[Equest-users] User Expression for Infiltration Neutral Zone Height
Melissa Crowe
MCrowe at cmta.com
Tue Mar 17 09:11:40 PDT 2020
Bless you ~Bill!
Melissa Crowe, LEED AP, BEMP
508-647-9200 ext. 1225
From: Bishop, Bill <bbishop at pathfinder-ea.com>
Sent: Tuesday, March 17, 2020 11:50 AM
To: Melissa Crowe <MCrowe at cmta.com>
Cc: equest-users at lists.onebuilding.org
Subject: RE: User Expression for Infiltration Neutral Zone Height
EXTERNAL SENDER: This email originated outside of CMTA. Do not click links or open attachments unless you know the sender and know the content is safe.
Hi Melissa,
Try this expression for NEUTRAL-ZONE-HT:
switch (#SV(#L("INF-METHOD")))
case 0 : unused
case 1 : unused
case 2 : NPL-(#P("Z")+#P("FLOOR-HEIGHT")/2)
case 3 : unused
case 4 : unused
default : unused
endswitch
Calculate the neutral pressure level for your building and replace "NPL" in the expression with the calculated value.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.pathfinder-ea.com%2f&c=E,1,qPB0DsRUr0WMdqWUEvL1tTWTEFT5xSxOOC-xugSomTepcNbJMhaU_GDBBBcxDCVU-RbEiCmMBPBahlrDpDknt-Bki2qtQaXMMuPRjkAK&typo=1>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image004.png at 01D5FC55.36631320] Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Melissa Crowe via Equest-users
Sent: Tuesday, March 17, 2020 10:13 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] User Expression for Infiltration Neutral Zone Height
Hi All
Help please, I am struggling with User Expression that calculates the Neutral Zone Height for high rise infiltration. It's something like:
((Parent("Z")-0)+Local("Height")/2)*-1+(BH/2 - BG)
Where:
BH = Building Height
BG = Total of Below Grade FL to FL Height
Also the default expression includes a switch statement. I don't thin I need a switch statement, so how is it formatted?
[cid:image005.png at 01D5FC55.36631320]
Thank you
[cid:image006.png at 01D5FC55.36631320]
Melissa Crowe, LEED AP, BEMP
Senior Mechanical/Energy Engineer
[cid:image007.jpg at 01D5FC55.36631320]
Boston Office
161 Worcester Road
Suite 305
Framingham, MA 01701
508-647-9200 ext. 1225
www.cmta.com<https://linkprotect.cudasvc.com/url?a=http%3a%2f%2fwww.cmta.com%2f&c=E,1,lEtAvzM8_wHHr-ZYsR1E4H7AYrDizKTrDQmA8vS6eiF1oUYFOvURMlyVKE7GJL2ngICsNZ_xKJJdBd9ZRV5Ghbr_XGn8sexmc_yxc5I_e14Mv-rkdLIsmvQ8&typo=1>
Follow us on Facebook<http://www.facebook.com/home.php#!/pages/CMTA-Consulting-Engineers/173253492360>, Twitter<https://twitter.com/CMTAEngineers> and LinkedIn<https://www.linkedin.com/company/cmta-inc.?trk=biz-companies-cym>
We've moved! Our new location is noted above - please update your records.
Look for an invitation to our Open House event to showcase the new space in the coming months.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/02816834/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/02816834/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1554 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/02816834/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 10024 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/02816834/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 36344 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/02816834/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 2311 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/02816834/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1903 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/02816834/attachment-0002.jpg>
More information about the Equest-users
mailing list