[Equest-users] Baseboard/Fin Tube Coil Loads
Brian Fountain
Brian.Fountain at sa-footprint.com
Thu Mar 12 06:43:52 PDT 2020
Hi Scott,
A couple of quick observations:
- While "OA Reset" is the default control mode for baseboard heating, I'd suggest that "Thermostatic" is more representative unless you specifically have a reason for applying a schedule to your baseboard heating. That change may resolve your issue.
- Baseboard heating is applied first before zonal heating - so size your baseboard heating carefully
- Baseboard heating is not autosized unless you are using DOE-2.3 so you will have to explicitly determine the baseboard heating capacities in the zones.
Beyond that you may wish to share the .inp and .pd2
Footprint
Brian Fountain
Associate
d 416 572 8501 m 416 562 6831
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Burger, Scott via Equest-users
Sent: March 12, 2020 9:32 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Baseboard/Fin Tube Coil Loads
CAUTION: EXTERNAL SENDER
Dear eQuest users,
I'm a novice eQuest user who is looking for some help regarding a project. I've used these forums to help gain knowledge of the program and how to make sense of it for my own work; however, the learning curve has been steep.
I developed a model for an existing building in conjunction with an onsite energy audit. In addition to completing an energy analysis and simulation, we are required to develop peak hourly heating and cooling loads for potential design of a GSHP system. The building uses 5 AHUs each with chilled water coils for cooling and hot water coils for heating. Additionally, there are fin tube radiators around most of the perimeter of the building. My goal is to disaggregate the ventilation portion of the peak heating load from the baseboard portion of the peak heating load. My research online and combing of forums indicates that disaggregating ventilation loads using eQuest is not a simple process. My initial thought was that if I can determine my hourly baseboard heating loads, I can estimate that the ventilation load accounts for the rest of the building's hourly heating load. However, after running an hourly simulation, I noticed that the heating coil load on the CIRCULATION-LOOPs that serve the fin-tube radiators show 0s from 1 AM - 6 AM. To verify this, I added "Zones" into my hourly simulation and noticed the same issue-0 "Baseboard heat output to zone (Btu/hr)" during hours from 1 AM - 6 AM.
On the Air-Side, the baseboards are controlled via "Outdoor Reset", and I verified that the reset schedule at the system level wouldn't preclude the baseboards from running during those hours. On the Water-Side, I verified that the boiler is in operation during those hours via a boiler schedule and that the actual HW loop serving the baseboards is in operation during those hours via a baseboard loop schedule as well. Based on the OA temp and the zone temperature (which is below the heating throttling range), the fin tube radiators should be operating per the model (and that's also how they operate the building in real life, as well).
I've seen the folks on this board provide some excellent advice and insight to other posters, so I hope you can do the same for me here! I'd appreciate if anyone can provide some insight as to why they think the fin tube radiators are showing 0 between 1 AM and 6 AM but seem to operate fine during the rest of the day. If you have any questions about the model or need more information, I am more than happy to oblige.
Scott Burger BEAP | Energy Engineer | scott.burger at arcadis.com<mailto:scott.burger at arcadis.com>
Arcadis
855 Route 146, Suite 210, Clifton Park, NY | 12065 | USA
T. +1 518 250 7261 | F. 518 371 2757
Connect with us! www.arcadis.com<http://www.arcadis.com/> | LinkedIn<https://www.linkedin.com/company/arcadis-north-america?trk=biz-companies-cym> | Twitter<http://www.twitter.com/arcadis_us> | Facebook<https://www.facebook.com/ArcadisNorthAmerica> | Connect App<http://arcad.is/eml-Connect>
[cid:image001.jpg at 01D5F852.1247F4D0]
[cid:image002.jpg at 01D5F852.1247F4D0]<http://arcad.is/eml-Connect>
Be green, leave it on the screen.
This email and any files transmitted with it are the property of Arcadis and its affiliates. All rights, including without limitation copyright, are reserved. This email contains information that may be confidential and may also be privileged. It is for the exclusive use of the intended recipient(s). If you are not an intended recipient, please note that any form of distribution, copying or use of this communication or the information in it is strictly prohibited and may be unlawful. If you have received this communication in error, please return it to the sender and then delete the email and destroy any copies of it. While reasonable precautions have been taken to ensure that no software or viruses are present in our emails, we cannot guarantee that this email or any attachment is virus free or has not been intercepted or changed. Any opinions or other information in this email that do not relate to the official business of Arcadis are neither given nor endorsed by it.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200312/140d0c69/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 2941 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200312/140d0c69/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2737 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200312/140d0c69/attachment-0001.jpg>
More information about the Equest-users
mailing list