[Equest-users] User Expression for Infiltration Neutral Zone Height
Bishop, Bill
bbishop at pathfinder-ea.com
Tue Mar 17 08:49:49 PDT 2020
Hi Melissa,
Try this expression for NEUTRAL-ZONE-HT:
switch (#SV(#L("INF-METHOD")))
case 0 : unused
case 1 : unused
case 2 : NPL-(#P("Z")+#P("FLOOR-HEIGHT")/2)
case 3 : unused
case 4 : unused
default : unused
endswitch
Calculate the neutral pressure level for your building and replace "NPL" in the expression with the calculated value.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image008.png at 01D5FC51.3BD960B0] Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Melissa Crowe via Equest-users
Sent: Tuesday, March 17, 2020 10:13 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] User Expression for Infiltration Neutral Zone Height
Hi All
Help please, I am struggling with User Expression that calculates the Neutral Zone Height for high rise infiltration. It's something like:
((Parent("Z")-0)+Local("Height")/2)*-1+(BH/2 - BG)
Where:
BH = Building Height
BG = Total of Below Grade FL to FL Height
Also the default expression includes a switch statement. I don't thin I need a switch statement, so how is it formatted?
[cid:image009.png at 01D5FC51.3BD960B0]
Thank you
[cid:image010.png at 01D5FC51.3BD960B0]
Melissa Crowe, LEED AP, BEMP
Senior Mechanical/Energy Engineer
[cid:image011.jpg at 01D5FC51.3BD960B0]
Boston Office
161 Worcester Road
Suite 305
Framingham, MA 01701
508-647-9200 ext. 1225
www.cmta.com<http://www.cmta.com/>
Follow us on Facebook<http://www.facebook.com/home.php#!/pages/CMTA-Consulting-Engineers/173253492360>, Twitter<https://twitter.com/CMTAEngineers> and LinkedIn<https://www.linkedin.com/company/cmta-inc.?trk=biz-companies-cym>
We've moved! Our new location is noted above - please update your records.
Look for an invitation to our Open House event to showcase the new space in the coming months.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/efdfcfa1/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/efdfcfa1/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 1554 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/efdfcfa1/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 10024 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/efdfcfa1/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 36344 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/efdfcfa1/attachment-0008.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.jpg
Type: image/jpeg
Size: 2311 bytes
Desc: image011.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/efdfcfa1/attachment-0007.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1903 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200317/efdfcfa1/attachment-0008.jpg>
More information about the Equest-users
mailing list