[Equest-users] System Selection for a Bus Terminal
Morteza Kasmai
morteza.kasmai at gmail.com
Wed Jan 22 11:49:39 PST 2020
David,
Thank you for your response. Do you mean, no matter how large is the
maintenance space, I can assume it as Heating Only Storage and select
System 9 for the baseline case.
Regards,
Morteza Kasmaei
Senior Architect
LEED AP BD+C, GGP
On Wed, Jan 22, 2020 at 2:18 PM David Eldridge <DEldridge at grummanbutkus.com>
wrote:
> The maintenance area and the office sections could be treated separately
> for their entry into the system selection table if you didn’t do that
> already. The operating hours, loads, and ventilation requirements would
> support separate systems for the two areas.
>
> DSE Mobile
> 773.490.5038
>
> On Jan 22, 2020, at 12:54 PM, Morteza Kasmai via Equest-users <
> equest-users at lists.onebuilding.org> wrote:
>
>
>
> Hello all,
>
> This is a bus maintenance/terminal that pursues LEED v4 platinum. 85% of
> the spaces in the proposed design have heating and ventilation system only
> with no cooling. The remaining 15% of the spaces will be conditioned with
> chilled beam, HW heating and DOAS with heat recovery. The HVAC system for
> the baseline case is System 7 per ASHRAE table G3.1.1A.
>
>
> What is the appropriate system for the heating ventilating spaces in both
> of the models? Should I assume cooling system identical to System 7 with
> high cooling temperature per Table G3.1.10 or I can assume as designed
> system for the proposed model and system 9 for the baseline case?
>
>
> As usual, thank you for your help.
>
> Morteza
>
> Morteza Kasmaei
> Senior Architect
> LEED AP BD+C, GGP
>
>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200122/b341b4d4/attachment.html>
More information about the Equest-users
mailing list