[Equest-users] DOAS and Fan Coils
Matthew S. Garlick
msg at tbcxinc.com
Fri Jan 17 08:21:35 PST 2020
Thanks for the responses! Unfortunately adding design days didn't help. I still get the following errors:
With just four pipe fan coil system:
**WARNING**********************************************************************
DOAS System: ERV-1 does not serve any
any systems (or zones), and will not be simulated.
**WARNING********************************************************************** (This x50)
PredictX parabolic solution failed. Please
send this input and weather file to program developers 3015
***ERROR***********************************************************************
Heat-Exchanger: HSouth Perim Zn (T.S40) UA calculation
failed to converge.
***ERROR***********************************************************************
Heat-Exchanger: HWSW Perim Zn (G.WSW5) UA calculation
failed to converge.
***ERROR***********************************************************************
Fatal HVAC simulation errors.
With the DOAS serving the fan coil system (No heat recovery) and delivering OA to conditioned zones:
***NOTE************************************************************************
Convergence issues in Design-Day mode 14
Hours Slow: 8; Hours Failed: 0
***ERROR***********************************************************************
Heat-Exchanger: HWest Perim Zn (M.W10) UA calculation
failed to converge.
***ERROR***********************************************************************
Heat-Exchanger: HEast Perim Zn (M.E12) UA calculation
failed to converge.
***ERROR***********************************************************************
Fatal HVAC simulation errors.
With the DOAS and heat recovery serving the fan coil system:
***NOTE************************************************************************
Convergence issues in Design-Day mode 14
Hours Slow: 7; Hours Failed: 138
**WARNING********************************************************************** (this x50)
PredictX parabolic solution failed. Please
send this input and weather file to program developers 3015
***ERROR***********************************************************************
Heat-Exchanger: HSouth Perim Zn (M.S13) UA calculation
failed to converge.
***ERROR***********************************************************************
Heat-Exchanger: HWSW Perim Zn (T.WSW41) UA calculation
failed to converge.
***ERROR***********************************************************************
Heat-Exchanger: HNorth Perim Zn (G.N8) UA calculation
failed to converge.
***ERROR***********************************************************************
Heat-Exchanger: HSouth Perim Zn (Mb.S22) UA calculation
failed to converge.
***ERROR***********************************************************************
Fatal HVAC simulation errors.
I tried switching the weather file (This was a custom built file) and got the same errors so I don't think the error lies there. I've attached the INP, PD2 (3.65 build 7175) and weather file for anyone with the time and desire to look into it.
Thanks again for the help, you guys rock!
[TBCx]
Matt Garlick, CxA, CEM, BEMP
Mobile: 801-907-5654
From: Nicholas Caton <Nicholas.Caton at se.com>
Sent: Thursday, January 16, 2020 9:19 PM
To: Matthew S. Garlick <msg at tbcxinc.com>
Cc: equest-users at lists.onebuilding.org; Jeff Hirsch <james.j.hirsch at gmail.com>
Subject: RE: DOAS and Fan Coils
Matt,
Well-documented!
It's been somewhat established through a couple threads over the past few months that "convergence errors" can sometimes, if not always, be related to difficulties in the system sizing portion of the simulation, and in those scenarios may be resolved by providing DESIGN-DAY inputs and/or manually specifying coil capacities you are relying on eQuest to auto-size.
You might check this possibility off the list by navigating to your first tab (Project & Site), deleting any design days you see there in the component tree, then importing the attached to see if that has any effect.
I believe references to convergence in the errors can also sometimes be a red herring, but in this case I'm not seeing some related telltale language in those screen snips. If you do encounter something to the effect of "MsgBomb call argument: " followed by some number of digits that is something you'll want to document/share as well.
~Nick
[cid:image005.png at 01D515A3.47EDD880]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Energy and Sustainability Services
Energy Performance Contracting
D
M
E
913 . 564 . 6361
785 . 410 . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
[cid:image006.png at 01D515A3.47EDD880]
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Matthew S. Garlick via Equest-users
Sent: Thursday, January 16, 2020 6:41 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] DOAS and Fan Coils
Howdy,
I'm trying to simulate a four pipe fan coil system with a DOAS ERV providing outdoor air in DOE 2.3 and getting some errors I haven't been able to figure out, I'm hoping someone here knows the answer!
The fan coil system runs by itself, connected to a campus CHW and steam loop, though I get the following error in my sim file:
***ERROR***********************************************************************
Heat-Exchanger: L1West Perim Zn (G.W1) UA calculation
failed to converge.
This seems to be a random zone and switches every time I run it. Besides defining OA flow at the zone, there are no other custom inputs at this time on the zone. When I add the DOAS (without the ERV) to the "OA From" field in the fan coil system, I get an aborted simulation and the following errors:
***NOTE************************************************************************
Convergence issues in Design-Day mode 14
Hours Slow: 3209; Hours Failed: 0
***ERROR***********************************************************************
Heat-Exchanger: HENE Perim Zn (M.ENE16) UA calculation
failed to converge.
***ERROR***********************************************************************
Heat-Exchanger: HSouth Perim Zn (Mb.S22) UA calculation
failed to converge.
***ERROR***********************************************************************
Fatal HVAC simulation errors.
Adding the ERV to the DOAS gets me a new set of errors:
***NOTE************************************************************************
Convergence issues in Design-Day mode 14
Hours Slow: 3384; Hours Failed: 1834
***ERROR***********************************************************************
Heat-Exchanger: HNorth Perim Zn (M.N17) UA calculation
failed to converge.
**WARNING**********************************************************************
PredictX parabolic solution failed. Please
send this input and weather file to program developers 3015
***ERROR***********************************************************************
Heat-Exchanger: HEast Perim Zn (T.E39) UA calculation
failed to converge.
***ERROR***********************************************************************
Fatal HVAC simulation errors.
Same notes and warnings as before but it adds the PredictX warning around 50 times (I edited the above).
I tried stepping back to DOE 2.2 but of course you can't define a DOAS in that engine and in 2.2 and 2.3 I'm unable to put an ERV on a fan coil system type.
So then, can anyone shine a light on what's going on?
[TBCx]
Matt Garlick, CxA, CEM, BEMP
Building Efficiency Engineer | TBCx
E-mail: msg at tbcxinc.com<mailto:msg at tbcxinc.com>
Mobile: 801-907-5654
Direct: 801-401-9492
324 S. State Street, Suite 400
Salt Lake City, UT 84111
www.tbcxinc.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Ftbcxinc.com%2F&data=02%7C01%7CNicholas.Caton%40se.com%7C76063b4b33a54a126de208d79ae5fa2f%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637148184845936058&sdata=rMYhO7OSmLsV9DMm%2BWLGmKuJkkjU2AmFLw9P%2BkloypU%3D&reserved=0>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200117/1fe1abf9/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200117/1fe1abf9/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200117/1fe1abf9/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: UT_LOGAN-CACHE-AP_724796_TYP.BINM
Type: application/octet-stream
Size: 185856 bytes
Desc: UT_LOGAN-CACHE-AP_724796_TYP.BINM
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200117/1fe1abf9/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Mountain View Housing_Proposed.pd2
Type: application/octet-stream
Size: 27067 bytes
Desc: Mountain View Housing_Proposed.pd2
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200117/1fe1abf9/attachment-0001.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Mountain View Housing_Proposed.inp
Type: application/octet-stream
Size: 133691 bytes
Desc: Mountain View Housing_Proposed.inp
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200117/1fe1abf9/attachment-0002.obj>
More information about the Equest-users
mailing list