[Equest-users] Custom Keywords and BDLKEY file

Aaron Powers caaronpowers at gmail.com
Fri Feb 14 12:50:47 PST 2020


Piggybacking a little off of Bill's post from earlier this week on keyword
expressions, I wanted to get people thinking about the possibilities/pros
and cons if one is able to add custom keywords and expressions (i.e. in
addition to the one's packaged with the standard eQuest release).  In my
opinion, this is a huge advantage to eQuest/DOE2 in that the interface can
be tweaked for individual preferences without changing the underlying
calculations.  As an example (and for anyone brave enough to try it out,
I've attached a modified BDLKEY.BIN and BDLDFT.DAT file which go in your
DOE23 folder as well as a modified BDLDialogs file which goes in the
ScreensDOE23 folder), this modified BDLKEY file includes an additional
numeric keyword for windows called WWR(window to wall ratio).  Now assuming
that you have no more than one window defined per exterior wall, the BDLDFT
file can be edited to include the following expressions:

SET-DEFAULT FOR WINDOW
  HEIGHT {SQRT(#L("WWR"))*#P("HEIGHT")}
  WIDTH {SQRT(#L("WWR"))*#P("WIDTH")}
  X {0.5*(#P("WIDTH") -#L("WIDTH" ))}
  Y {0.5*(#P("HEIGHT") -#L("HEIGHT" ))}
..

Now the size and position of individual windows are controlled by a single
parameter, which is bound to each particular window (assuming you allow the
4 parameters above to default).

[image: image.png]

The major downside is that this is no longer complies with the standard
release, and one could end up with a nearly infinite number of eQuest
flavors depending on modifications to the keyword file.  Sharing files and
QCing years after the fact could become a nightmare.  A possible solution
to this problem would be the ability to add keywords on the fly, the way
that global parameters are, which are associated with individual .inp files
and not with the program itself.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200214/db69ff1c/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image.png
Type: image/png
Size: 48079 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200214/db69ff1c/attachment-0001.png>
-------------- next part --------------
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;
;   NEXT IDs TO USE:
;
;   TABDLG / TABPAGE / SUBTABPAGE:   3391
;
;   UI CONTROLS                  :  19485
;       (range reserved for Design Sizing version)  :  18000 - 18200
;                           NEXT DS Version Control :  18111
;
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 


;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;
; SAC/AFR Apr-May/09 Mods:  Increase dialog some sizes and integrate "C-" keywords into std keyword tabs
; SAC Nov/10 Mods:  Large number of controls removed and added to convert from DOE-2.2 -> 2.3 (design sizing version)
;
;  - large (SYSTEM) tabbed dialog size from "470, 710" to "570, 1030"
;
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;
; CONVERSION STEPS (PowerDOE 1 -> eQUEST):
;
; 1. Add BDL Command Edited (or NOTIMP) before Caption for dialogs, tabbed dialogs & tabbed dialog pages
;
; 2. Change tabbed dialog size from "310, 610" to "470, 710"
;
; 3. Change *control label and units label coordinates to be in relation to top-left and top-right corners of the control
;
; 4. Add two properties to each LABEL -> right shadowline X coord & ID of associated UI control (both 0 for none)
;    - also remove trailing ':'s from labels with shadowline extensions
;
; 5. Switch all ComboBox "Height of edit portion of control" values from 21 to 19
;
; 6. Switch all Edit "Height" values from 21 to 23
;
; 7. Switch all font settings of "ITALIC_UND" to "STD"
;
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 


 ;****************************************************************************************************************
 ; Bogus chars to replace:  apostrophe: ’
 ;
 ;
 ; SAC 6/30/03 - New Compliance Mode flags:
 ; AFR 5/11/09 - Expanded 6 and 7 for LEED ruleset.
 ;      1 => Display Tab/Control only if any compliance ruleset is loaded
 ;      2 => Display Tab/Control only if NO compliance ruleset is loaded
 ;      3 => Display Tab/Control regardless of whether or not a compliance ruleset is loaded
 ;      4 => Display Tab/Control only if a compliance ruleset is loaded that ALLOWS SBD analysis
 ;      5 => Display Tab/Control only if a compliance ruleset is loaded that DOES NOT allow SBD analysis
 ;      6 => Display Tab/Control only if a compliance ruleset is loaded that ALLOWS LEED analysis
 ;      7 => Display Tab/Control only if a compliance ruleset is loaded that DOES NOT allow LEED analysis
 ;      8 => Display Tab/Control only if  (a compliance ruleset is loaded that DOES NOT allow LEED analysis)
 ;                                   -OR- (jurisdictional QC reporting is selected)
 ;
 ;
 ;  16-bit - DATA WINDOWS (DATAWIN):
 ;	 16-bit -   Control Heading, Control ID, Help ID, User Level ID, Module Name, Height, System ID
 ;  16-bit - 
 ;  16-bit - DIAGRAM WINDOWS (DIAGWIN):
 ;	 16-bit -   Control Heading, Control ID, Help ID, User Level ID, Module Name, System ID
 ;
 ;  MODAL and NONMODAL DIALOG BOXES (MODDLG, NONMODDLG):
 ;		Control Heading, Dialog ID, Help ID, User Level ID, X-Coordinate, Y-Coordinate, Height, Width, 
 ;    Scale to Resolution Flag,
 ;   *SAC Added 2/3/99: Name of BDL command for which this dialog is the primary edit mechanism (or 'NOTIMP')
 ;    Caption, Command1 Name, Command1 Type, Keyword1 Name, Command1/Keyword1 
 ;    Array Index, Number of Places after the decimal, Units Flag, Trailing String1, Command2 Name, 
 ;    Command2 Type, Keyword2 Name, Command2/Keyword2 Array Index, Number of Places after the decimal, 
 ;    Units Flag, Trailing String2 
 ;    NOTE: -Max Non-Scaling Height = 480
 ;          -Max Non-Scaling Width  = 620
 ;          -Max Scaling Height     = 600
 ;          -Max Scaling Width      = 780
 ;          -If the Command1 Name and Keyword1 Name are NOTIMP, only the Command1/Keyword1 Array Index
 ;           needs to be entered.  The remaining parameters are not necessary. 
 ;          -If the Command1 Name and Keyword1 Name are not NOTIMP, the remaining parameters must be 
 ;           entered. (If Command2 Name and Keyword2 Name are NOTIMP, only the Command2/Keyword2 Array
 ;           Index needs to be entered.  The remaining parameters are not necessary.)
 ;
 ;  MODAL and NONMODAL TAB DIALOG BOXES (MODTABDLG, NONMODTABDLG):
 ;    Control Heading, Dialog ID, Help ID, User Level ID, X-Coordinate, Y-Coordinate, Height, Width, 
 ;    Scale to Resolution Flag,
 ;   *SAC Added 2/3/99: Name of BDL command for which this dialog is the primary edit mechanism (or 'NOTIMP')
 ;    Caption, Command1 Name, Command1 Type, Keyword1 Name, Command1/Keyword1 
 ;    Array Index, Number of Places after the decimal, Units Flag, Trailing String1, Command2 Name, 
 ;    Command2 Type, Keyword2 Name, Command2/Keyword2 Array, Index, Number of Places after the decimal, 
 ;    Units Flag, Trailing String2
 ;    NOTE: -The defined height and width is actually the height and width of the pages 
 ;           within the Tab Dialog.
 ;          -If the Command1 Name and Keyword1 Name are NOTIMP, only the Command1/Keyword1 Array Index
 ;           needs to be entered.  The remaining parameters are not necessary. 
 ;          -If the Command1 Name and Keyword1 Name are not NOTIMP, the remaining parameters must be 
 ;           entered. (If Command2 Name and Keyword2 Name are NOTIMP, only the Command2/Keyword2 Array
 ;           Index needs to be entered.  The remaining parameters are not necessary.)
 ;          -Max Non-Scaling Height = 360
 ;          -Max Non-Scaling Width  = 600
 ;          -Max Scaling Height     = 490
 ;          -Max Scaling Width      = 770
 ;
 ;  PAGES within TAB DIALOG BOXES (TABPAGE):
 ;    Control Heading, Page ID, Help ID, User Level ID,
 ;   *SAC added 5/18/00 - Compliance Flag (see legend above),
 ;   *SAC Added 2/3/99: Name of BDL command for which this tab is the primary edit mechanism (or 'NOTIMP')
 ;    Caption
 ;	
 ;  EDIT BOXES (EDIT):
 ;		Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Command Name, 
 ;    Command Type, Keyword Name, Command/Keyword Array Index, Font, X-Coordinate, Y-Coordinate, Height, 
 ;    Width, Number of Places After Decimal,
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above),
 ;    Label, Label Justification, Label X-Coordinate, 
 ;    Y-Coordinate, Units Flag, Units Justification, Units X-Coordinate, Units Y-Coordinate, 
 ;    (units table index if NOTIMP or eQUEST control), Status Bar Message
 ;
 ;  16-bit - NAVEDIT BOXES (NAVEDIT):
 ;	 16-bit - 	Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID,
 ;  16-bit -   Navigation ID, Command Name, Command Type, Keyword Name, Command/Keyword
 ;  16-bit -   Array Index, Secondary Command Name, Secondary Command Type, Secondary
 ;  16-bit -   Keyword Name, Secondary Command/Keyword Array Index, Font, X-Coordinate,
 ;  16-bit -   Y-Coordinate, Height, Width, Number of Places After Decimal, Label, Label
 ;  16-bit -   Justification, Label X-Coordinate, Y-Coordinate, Units Flag, Units 
 ;  16-bit -   Justification, Units X-Coordinate, Units Y-Coordinate, (units table index
 ;  16-bit -   if NOTIMP or eQUEST control), Status Bar Message
 ;
 ;  COMBO BOXES (COMBO):
 ;		Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Command Name, 
 ;    Command Type, Keyword Name, Command/Keyword Array Index, Font, X-Coordinate, Y-Coordinate, Height, 
 ;    Width, Height of edit portion of control,
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above),
 ;    Label, Label Justification, Label X-Coordinate, 
 ;    Y-Coordinate, Units Flag, Units Justification, Units X-Coordinate, Units Y-Coordinate, 
 ;    Status Bar Message
 ;
 ;  16-bit - MAPCOMBO BOX (MAPCOMBO):
 ;  16-bit -   Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Command Name, 
 ;  16-bit -   Command Type, Keyword Name, Command/Keyword Array Index, Font, X-Coordinate, Y-Coordinate, Height, 
 ;  16-bit -   Width, Height of edit portion of control, Label, Label Justification, Label X-Coordinate, 
 ;  16-bit -   Y-Coordinate, Units Flag, Units Justification, Units X-Coordinate, Units Y-Coordinate, 
 ;  16-bit -   Status Bar Message
 ;
 ;  BUTTONS (BUTTON):
 ;    Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Navigation ID (action code),
 ;   *SAC added 6/22/00 (FILE_STRUCT_VERSION >= 3) - Secondary Navigation ID (dlg or spread ctrl ID)
 ;    Font, X-Coordinate, Y-Coordinate, Height, Width,
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above),
 ;    Label, Status Bar Message
 ;
 ;  CHECKBOX BUTTONS (CHECKBOX):
 ;    Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Command Name, Command Type,
 ;    Keyword Name, Command/Keyword Array Index, Font, X-Coordinate, Y-Coordinate, Height, Width,
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above),
 ;    Label, Label Justification, Status Bar Message
 ;       EXAMPLE:   CHECKBOX, 19027, 19027,   776, 1,  WINDOW, 0, SETBACK, -1, STD, 135, 155,  17, 100, 3, "Is Setback", LEFT, "-status msg-"
 ;
 ;  RADIO BUTTONS (RADIOFIRST, RADIONEXT):
 ;    Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, ID of Window to Redraw 
 ;    if Selected, Command Name, Command Type, Keyword Name, Command/Keyword Array Index, 
 ;    Command/Keyword Value (numeric), Font, X-Coordinate, Y-Coordinate, Height, Width,
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above),
 ;    Label, Label Justification, Status Bar Message
 ;
 ;  16-bit - BITMAP BUTTONS (BMPBUTTON):
 ;  16-bit -   Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Navigation ID, Font, 
 ;  16-bit -   Button Width, Status Bar Message
 ;  16-bit - 
 ;  16-bit - ICON BUTTONS (ICONBUTTON):
 ;  16-bit -   Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, IconCase data ID
 ;  16-bit -   Single Click Module, Single Click DOE-2 Parameter Name, Single Click DOE-2 Parameter Value,
 ;  16-bit -   Double Click Module or Navigation ID, Double Click DOE-2 Parameter Name, Double Click DOE-2
 ;  16-bit -   Parameter Value, Font, X-Coordinate, Y-Coordinate, Height, Width, Reposition Flag, Install/
 ;  16-bit -   Uninstall Index, Label1, Label2, Label3, Short Label1, Short Label2, Short Label3, Bitmap Name,
 ;  16-bit -   Label Placement, X Label Offset (- left, + right), Y Label Offset (- up, + down),  Status Bar Message
 ;  16-bit - 
 ;  16-bit - BITMAPS (BITMAP)
 ;  16-bit -   Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Command Name, Command Type, 
 ;  16-bit -   KeyWord Name, Command/Keyword Array Index, X-Coordinate, Y-Coordinate, Height (- Value will center 
 ;  16-bit -   vertically with Y-Coordinate as offset), Width (- Value will center horizontally with X-Coordinate 
 ;  16-bit -   as offset), Stretch Bitmap(0/1), Maintain Aspect Ratio(0/1), Index into Bitmap.dat file
 ;  16-bit - 
 ;  16-bit - METAFILES (METAFILE)
 ;  16-bit -   Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Command Name, Command Type, 
 ;  16-bit -   KeyWord Name, Command/Keyword Array Index, X-Coordinate, Y-Coordinate, Height (- Value will center 
 ;  16-bit -   vertically with Y-Coordinate as offset), Width (- Value will center horizontally with X-Coordinate 
 ;  16-bit -   as offset), Stretch Bitmap(0/1), Maintain Aspect Ratio(0/1), Index into Metafile.dat file
 ;  
 ;  PICTURES (PICTURE) - replaces BITMAPs and METAFILEs
 ;    Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Command Name, Command Type, 
 ;    KeyWord Name, Command/Keyword Array Index, X-Coordinate, Y-Coordinate, Height (- Value will center 
 ;    vertically with Y-Coordinate as offset), Width (- Value will center horizontally with X-Coordinate as offset),
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above),
 ;    Stretch Bitmap(0/1), Maintain Aspect Ratio(0/1), Background Red (0-255), Background Green (0-255),
 ;    Background Blue (0-255), Small Font/Resource Index into PictureIDs.txt file, Large Font/Resource Index into
 ;    PictureIDs.txt file
 ;
 ;  16-bit - GRAPHS (GRAPH)
 ;  16-bit -    Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Command Name, Command Type, 
 ;  16-bit -    KeyWord Name, Command/Keyword Array Index, X-Coordinate, Y-Coordinate, Height, Width, Scale to 
 ;  16-bit -    System Font (0/1), Scale to Screen Resolution (0/1)
 ;
 ;  SPREAD SHEETS (SPREAD):
 ;    Control Heading, Control ID, Item Help ID, Topic Help ID, User Level ID, Navigation ID, Command Name, 
 ;    Command Type, Keyword Name, Array Index, Font, X-Coordinate, Y-Coordinate, Height, Width, Row Height, 
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above),
 ;    Label, Label Justification, Label X-Coordinate, Label Y-Coordinate, Units Flag, Units Justification,
 ;    Units X-Coordinate, Units Y-Coordinate, Status Bar Message      
 ;  
 ;  STATIC (STATIC):
 ;    Control Heading, User Level ID, Command Name, Command Type, Keyword Name, Array or Units Table Index, 
 ;    Has Subcommand Flag, (if Has Subcommand Flag = 1, SubCommand Name, SubCommand Type, SubKeyword Name),
 ;    Number of Places after the decimal or number of characters, X-Coordinate, Y-Coordinate,
 ;    Maximum Width (-1 for none), Font, Justification, Label 1, Label 2, Units Flag (0/1),
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above)
 ;
 ;  LABELS (LABEL):
 ;	 	Control Heading, Label, Font, Label Justification, X-Coordinate, Y-Coordinate, Scale Coordinates
 ;    to System Font Size, Scale Coordinates to Screen Resolution, Scale Coordinates to Diagram Size,
 ;   *SAC Added 2/5/99: Right coordinate for shadowline (0 for no shadowline)
 ;   *SAC Added 2/5/99: ID of associated control (or 0 for no associated ctrl) (used to select font color)
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above)
 ;
 ;  LINES (LINE):
 ;	 	Control Heading, From X-Coord, From Y-Coord, To X-Coord, To Y-Coord, Thickness (-1 for shadowline),
 ;    Style (SOLID, DASH, DOT, DASHDOT, DASHDOTDOT), Red, Green, Blue, Arrow Flag (NONE, THIN, THICK), Scale
 ;    Coordinates to System Font Size, Scale Coordinates to Screen Resolution, Scale Coordinates to Diagram Size
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above)
 ;  
 ;  RECTANGLES (RECT):
 ;    Control Heading, Top Y-Coord, Bottom Y-Coord, Left X-Coord, Right X-Coord, Fill Red, Fill Green, 
 ;    Fill Blue (No Fill: 0 for Fill Red, Fill Green, Fill Blue), Boundary Thickness (0 for No Boundary), 
 ;    Boundary Red, Boundary Green, Boundary Blue, Round Height, Round Width, Scale Coordinates
 ;    to System Font Size, Scale Coordinates to Screen Resolution, Scale Coordinates to Diagram Size
 ;   *SAC added 5/17/00 - Compliance Flag (see legend above)
 ;       (Square corners      => 0 for both Round Height and Round Width)
 ;       (Bottom or Right < 0 => extend to limits of current display - Bot/Rgt + 1)
 ;       (Fill/Boundary Red/Green/Blue = -1 => No action (no fill /boundary drawn) )
 ;       (     "              "        = -2 => Draw Fill/Boundary with default ButtonFace color )
 ;
 ;  CASE Statements (CASE):
 ;    Control Heading, Command Name, Command Type, Keyword Name, Array Index, Logical Operator (=, <, >,
 ;    <=, >=, !=), Number of Values to Compare, Values...
 ;    NOTE: -For for else statements:
 ;           Control Heading, "ELSE". (For example: CASE, ELSE)
 ;          -All CASE statements must be followed by a corresponding ENDCASE.    
 ;
 ;  SPREAD:
 ;		Control Heading, Control ID, Unique DOE-2 ID, Elements to display flag
 ;     (ALL or ACTIVE), Key Type (NONE, SINGLE_FILL, SINGLE_NO_FILL, PAIR, 
 ;     TRIPLET), Number of configurations,
 ;       For each configuration in the spreadsheet:
 ;       Configuration BDL Command, BDL Command Type, Spreadsheet Mode (NORMAL 
 ;       or TRANSPOSE), Row Header ID (or "NONE"), Row Header Font, Row Header 
 ;       Column Width, Column Header Row Height, Number of Locked Columns, Total
 ;       Number of Columns,
 ;         For each column in the spreadsheet configuration:
 ;         Column Title, Column Width, Misc Data (# chars, decimal precision),
 ;         Display Units in label flag, Editable, Command Type, 
 ;         Compliance Flag, *AFR 4/30/09 - added, mostly to set the background color to make the keywords more easily readable.
 ;         BDL Keyword, 
 ;         Array Index, Item Help ID, Topic Help ID, Has Subcommand (0/1), (if
 ;         Has Subcommand is 1, Command, Com Type, Keyword, Array Index), Status
 ;         Bar Message
 ;				
 ;  SPREADHEADER:
 ;     Control Heading, Header Type, Number of Headers, Header, ...
 ;
 ;  SPECIAL RESERVED BUTTON IDs
 ;       OK            1
 ;       CANCEL        2
 ;       ABORT         3
 ;       RETRY         4
 ;       IGNORE        5
 ;       YES           6
 ;       NO            7
 ;       DEFAULT       8 
 ;
 ;
 ;  BUTTON NAVIGATION IDs / ACTION CODES:
 ;       Value     Description
 ;       --------------------------------------------------------------------------
 ;         90  =>  Browse for wizard weather file
 ;         91  =>  Present EEM details dialog
 ;         92  =>  Present BDL Tabbed Dialog
 ;         93  =>  Add to optional list keyword array
 ;         94  =>  Insert item into optional list keyword array
 ;         95  =>  Delete element of optional list keyword array
 ;
 ;  BUTTON SECONDARY NAVIGATION IDs / Dlg, Tabbed Dlg or Spreadsheet Ctrl IDs:
 ;       Action    Valid Range for
 ;        Code     Secondary Nav ID
 ;       --------------------------------------------------------------------------
 ;         90  =>  - unused -
 ;         91  =>  1-based index of EEM object to present the detailed dialog for
 ;         92  =>  ID of Individual Dialog Tab to Present
 ;         93  =>  ID of spreadsheet control which provides access to the optional list
 ;         94  =>  ID of spreadsheet control which provides access to the optional list
 ;         95  =>  ID of spreadsheet control which provides access to the optional list
 ;
 ;
 ;****************************************************************************************************************
 ; SAC 11/30/10 - added mod to force re-read of text file due to update in binary format

FILE_STRUCT_VERSION, 4 ; AFR 4/30/09 - changed file version to support adding ComplianceFlag to SPREAD

;*******************************************************************************
; SpreadSheet Headers
;*******************************************************************************

   SPREADHEADER, NUMBERS, 1, "*"

   SPREADHEADER, MONTHLONG, 12, "January", "February", "March", "April", "May", "June", 
      "July", "August", "September", "October", "November", "December"

   SPREADHEADER, XYZ, 3, "X", "Y", "Z"   
      
   SPREADHEADER, ANGLE, 11, "0°", "10°", "20°", "30°", "40°", "50°", "60°", "70°", "80°", "90°", "Hemis"   
   
; JJH 1/17/06 - GSHP mods
   SPREADHEADER, GFUNC, 27,"Ln(t/ts) -8.5","Ln(t/ts) -7.8","Ln(t/ts) -7.2","Ln(t/ts) -6.5",
                "Ln(t/ts) -5.9","Ln(t/ts) -5.2","Ln(t/ts) -4.5","Ln(t/ts) -3.963","Ln(t/ts) -3.27",
                "Ln(t/ts) -2.864","Ln(t/ts) -2.577","Ln(t/ts) -2.171","Ln(t/ts) -1.884","Ln(t/ts) -1.191",
                "Ln(t/ts) -0.497","Ln(t/ts) -0.274","Ln(t/ts) -0.051","Ln(t/ts) 0.196","Ln(t/ts) 0.419",
                "Ln(t/ts) 0.642","Ln(t/ts) 0.873","Ln(t/ts) 1.112","Ln(t/ts) 1.335","Ln(t/ts) 1.679",
                "Ln(t/ts) 2.028","Ln(t/ts) 2.275","Ln(t/ts) 3.003"


;*******************************************************************************
; SpreadSheets
;*******************************************************************************

; AFR 4/30/09 - added the ComplianceFlag varaible just before the keyword name in each column defination.

   ;*****   Global Parameters Spreadsheets   *****

   SPREAD, ParamSpread, 265, ALL, NONE, 1,
			   PARAMETER, -1, NORMAL, NUMBERS, STD, 30, 20, 1, 3
			   	"Parameter Name",   150, 32, 0, 0, 0, 3, NAME,           -1,   998,   995, 0, "Name of parameter"
			   	"Parameter Type",   120, 32, 0, 0, 0, 3, PARAM-TYPE,     -1,   997,   995, 0, ""
			   	"Parameter Value",  150, 32, 0, 1, 0, 3, PARAM-VALUE,    -1,   996,   995, 0, ""


   ;*****   Holidays Spreadsheet   *****

   SPREAD, HolidaySpread, 676, ACTIVE, NONE, 1, 
			   HOLIDAYS, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 2
               "Months",  55,  0, 1, 1,  1, 3, MONTHS,    -1,  691,  12543,  0, "The month number of each custom Holiday"
               "Days",    50,  0, 1, 1,  1, 3, DAYS,      -1,  685,  12543,  0, "The day number of each custom Holiday"


   ;*****   Site Parameters Spreadsheets   *****

   SPREAD, SiteGrndTemp, 165, ACTIVE, NONE, 1, 
   			SITE-PARAMETERS, -1, NORMAL, MONTHLONG, STD, 100, 20, 1, 1
   		      "Ground Temp",   115,  2, 1, 1, 0, 3, GROUND-T,           -1,   811,   0, 0, ""
            
   SPREAD, SiteSolar, 175, ACTIVE, NONE, 1, 
   			SITE-PARAMETERS, -1, NORMAL, MONTHLONG, STD, 100, 20, 3, 3
               "Clearness #",   100,  2, 0, 1, 0, 3, CLEARNESS-NUMBER,   -1, 63059,   0, 0, ""
               "ATM Moisture",  100,  2, 0, 1, 0, 3, ATM-MOISTURE,       -1, 63060, 758, 0, ""
               "ATM Turbidity", 100,  2, 0, 1, 0, 3, ATM-TURBIDITY,      -1, 63061,   0, 0, ""

   SPREAD, SiteTerrain, 185, ACTIVE, NONE, 1, 
   			SITE-PARAMETERS, -1, NORMAL, MONTHLONG, STD, 100, 20, 1, 1
      			"WS-Height",     100,  2, 1, 1, 0, 3, WS-HEIGHT-LIST,     -1, 11504, 773, 0, "Height above ground at which wind speed data were recorded (monthly values)"


   ;*****   Annual Schedule Spreadsheets   *****

   SPREAD, AnnSchSpread1, 656, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1,  1, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1,  1, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1,  1, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread2, 657, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1,  2, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1,  2, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1,  2, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread3, 658, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1,  3, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1,  3, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1,  3, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread4, 659, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1,  4, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1,  4, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1,  4, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread5, 660, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1,  5, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1,  5, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1,  5, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread6, 661, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1,  6, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1,  6, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1,  6, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread7, 662, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1,  7, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1,  7, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1,  7, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread8, 663, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1,  8, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1,  8, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1,  8, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread9, 664, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1,  9, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1,  9, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1,  9, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread10, 665, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1, 10, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1, 10, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1, 10, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread11, 666, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1, 11, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1, 11, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1, 11, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"

   SPREAD, AnnSchSpread12, 667, ACTIVE, NONE, 1, 
   			SCHEDULE, -1, NORMAL, NUMBERS, STD, 35, 36, 0, 3          ;    ItmHlp  TpcHlp
               "Ending Month",    50,  0, 1, 1, 12, 3, MONTH,          -1,  31798,  31793,  0, "Ending month for this week schedule assignment"
               "Ending Day",      50,  0, 1, 1, 12, 3, DAY,            -1,  31799,  31793,  0, "Day of the ending month for this week schedule assignment"
               "Week Schedule",  250, 32, 1, 1, 12, 3, WEEK-SCHEDULES, -1,  31797,  31793,  0, "Week schedule assigned for the period ending on the indicated month/day"


   ;*****   Space Spreadsheets   *****

; SAC 11/22/10 - added EQUIP-TO-RETURN
   SPREAD, SpaceEquipSpread, 700, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 30, 49, 0, 8                 ;    ItmHlp  TpcHlp
               "Equipment Schedule",  230, 32, 1, 1,  1, 3, EQUIP-SCHEDULE,   -1,  12070,  3002,  0, "Name of schedule that controls the equipment energy use in the selected zone"
               "Input Power Density",  80,  3, 1, 1,  1, 3, EQUIPMENT-W/AREA, -1,  12071,  3002,  0, "Equipment input power density for the selected space (an alternative to Input Power)"
               "Input Power",          60,  2, 1, 1,  1, 3, EQUIPMENT-KW,     -1,  12072,  3002,  0, "Total equipment input power for the selected space (an alternative to Input Power Density)"
               "Equip to Return",      60,  2, 1, 1,  1, 3, EQUIP-TO-RETURN,  -1,      0,  3002,  0, "Fraction of equipment power consumption that appears in the return air stream space as heat/latent"
               "Sensible HG",          55,  2, 1, 1,  1, 3, EQUIP-SENSIBLE,   -1,    727,  3002,  0, "Fraction of Equipment Power Input released to the space as sensible heat"
               "Latent HG",            55,  2, 1, 1,  1, 3, EQUIP-LATENT,     -1,  12073,  3002,  0, "Fraction of Equipment Power Input released to the space as latent heat"
               "Curve of Power f(T)", 150, 32, 1, 1,  1, 3, EQUIP-PWR-FT,     -1,      0,  3002,  0, "Name of curve that modifies equipment power and heat gain as a function of space temperature"
               "Pwr f(T) Rated T",     60,  1, 1, 1,  1, 3, EQUIP-RATED-T,    -1,      0,  3002,  0, "the temperature at which the equipment power is defined (used only when curve of Power f(T) defined)"

;  TWV 11/28/11 - Changed out Input Power row, SOURCE-BTU/HR Keyword replaced with SOURCE-POWER
   SPREAD, SpaceIntSrcSpread, 701, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 5                 ;    ItmHlp  TpcHlp
               "Source Schedule",     230, 32, 1, 1,  1, 3, SOURCE-SCHEDULE,  -1,    726,  3002,  0, "Schedule that controls the source energy use in the selected space"
               "Source Type",         100,  2, 1, 1,  1, 3, SOURCE-TYPE,      -1,    725,  3002,  0, "Type of source energy use in the selected space"
               "Input Power",          80,  1, 1, 1,  1, 3, SOURCE-POWER,    -1,    724,  3002,  0, "Total source input power for the selected space"
               "Sensible HG",          80,  2, 1, 1,  1, 3, SOURCE-SENSIBLE,  -1,    722,  3002,  0, "Fraction of source power input in the selected space that is sensible"
               "Latent HG",            80,  2, 1, 1,  1, 3, SOURCE-LATENT,    -1,    723,  3002,  0, "Fraction of source power input in the selected space that is latent"

; SAC 3/27/09 - added 6 columns to each space lighting spreadsheet to handle input of keywords switched from single elements to arrays
   SPREAD, SpaceLightPow, 726, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 20, 49, 0, 10
   		      "Power Density",          60,  3, 1, 1, 0, 3, LIGHTING-W/AREA,  -1, 12028, 32084, 0, "Max power consumption of main overhead lights in zone, per square foot of floor area"
   		      "Power",                  60,  2, 1, 1, 0, 3, LIGHTING-KW,      -1, 62015, 32084, 0, "Maximum amount of power consumed by the overhead lighting subsystem"
   		      "Lighting Type",         110,  2, 0, 1, 0, 3, LIGHTING-TYPE,    -1, 62014, 32084, 0, "Defines distribution of heat from lights; to return air, radiative/convective fractions, etc."
   		      "Schedule",              155,  2, 0, 1, 0, 3, LIGHTING-SCHEDUL, -1, 62013, 32084, 0, "A fractional schedule that adjusts the lighting subsystem's power consumption each hour"
   		      "Light to Space",         60,  2, 1, 1, 0, 3, LIGHT-TO-SPACE,   -1,     0, 32084, 0, "Fraction of the lighting power consumption that appears in the space as heat"
   		      "Light to Adj Spc",       60,  2, 1, 1, 0, 3, LIGHT-TO-OTHER,   -1,     0, 32084, 0, "Fraction of the lighting power consumption that appears in an adjacent space as heat"
   		      "Light to Return",        60,  2, 1, 1, 0, 3, LIGHT-TO-RETURN,  -1,     0, 32084, 0, "Fraction of lighting power consumption that appears in the return air stream space as heat"
   		      "Rad Frac This Space",    60,  2, 0, 1, 0, 3, LIGHT-RAD-FRAC,   -1,     0, 32084, 0, "The fraction of heat (from lights) in the space that is radiative (the remainder is convective)"
   		      "Rad Frac Adj Space",     60,  2, 0, 1, 0, 3, OTHER-RAD-FRAC,   -1,     0, 32084, 0, "The fraction of heat (from lights) appearing in an adjacent space that is radiative (the remainder is convective)"
     "Adjacent Space Light Heat To", 140,  2, 1, 1, 0, 3, LIGHT-HEAT-TO,    -1,     0, 32084, 0, "An adjacent space that receives the Fraction of Light Heat to Adjacent Space"

   SPREAD, SpaceLightSys, 716, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 20, 49, 0, 12
   		      "Lighting System",       150,  2, 0, 1, 0, 3, LIGHTING-SYSTEM,  -1, 13584, 32084, 0, ""
   		      "Power",                  50,  2, 1, 1, 0, 3, LIGHTING-KW,      -1, 62015, 32084, 0, "Maximum amount of power consumed by the overhead lighting subsystem"
   		      "Number of Luminaires",   75,  2, 0, 1, 0, 3, NO-OF-LUMINAIRES, -1, 62019,     0, 0, "No. of luminaires in the lighting subsystem, of the type defined by the chosen Lighting System"
   		      "Illuminance",            75,  2, 1, 1, 0, 3, ELEC-ILLUMINANCE, -1,  3005,     0, 0, "Desired average illuminance from each of the lighting subsystems"
   		      "Ceil to Lum Dist",       80,  2, 1, 1, 0, 3, CEIL-TO-LUM-DIS,  -1, 62017,     0, 0, "Distance from the ceiling to the center plane of the luminaires"
   		      "Schedule",              155,  2, 0, 1, 0, 3, LIGHTING-SCHEDUL, -1, 62013, 32084, 0, "A fractional schedule that adjusts the lighting subsystem's power consumption each hour"
   		      "Light to Space",         60,  2, 1, 1, 0, 3, LIGHT-TO-SPACE,   -1,     0, 32084, 0, "Fraction of the lighting power consumption that appears in the space as heat"
   		      "Light to Adj Spc",       60,  2, 1, 1, 0, 3, LIGHT-TO-OTHER,   -1,     0, 32084, 0, "Fraction of the lighting power consumption that appears in an adjacent space as heat"
   		      "Light to Return",        60,  2, 1, 1, 0, 3, LIGHT-TO-RETURN,  -1,     0, 32084, 0, "Fraction of lighting power consumption that appears in the return air stream space as heat"
   		      "Rad Frac This Space",    60,  2, 0, 1, 0, 3, LIGHT-RAD-FRAC,   -1,     0, 32084, 0, "The fraction of heat (from lights) in the space that is radiative (the remainder is convective)"
   		      "Rad Frac Adj Space",     60,  2, 0, 1, 0, 3, OTHER-RAD-FRAC,   -1,     0, 32084, 0, "The fraction of heat (from lights) appearing in an adjacent space that is radiative (the remainder is convective)"
     "Adjacent Space Light Heat To", 140,  2, 1, 1, 0, 3, LIGHT-HEAT-TO,    -1,     0, 32084, 0, "An adjacent space that receives the Fraction of Light Heat to Adjacent Space"

; AFR 5/12/09 - added new spread for title 24 compliance.
   SPREAD, SpaceLightComp, 756, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 20, 49, 0, 6
   		      "Lighting Area Type",         150,  0, 0, 1, 0, 1, C-LTG-AREA-TYP,   -1, 0, 0, 0, ""
   		      "Category",                   150,  0, 0, 1, 0, 1, C-AVAIL-OCC-TYPE, -1, 0, 0, 0, ""
   		      "Area",                        85,  0, 1, 1, 0, 1, C-LTG-AREA,       -1, 0, 0, 0, ""
   		      "Daylight Controls Required",  85,  0, 0, 1, 0, 1, C-DAYLT-CTRL-REQ, -1, 0, 0, 0, ""
   		      "Controlled Lighting",         85,  3, 1, 1, 0, 1, C-LTG-CTRL-KW,    -1, 0, 0, 0, ""
   		      "Control Scheme",             150,  0, 0, 1, 0, 1, C-LTG-CTRL-TYPE,  -1, 0, 0, 0, ""

;   SPREAD, SpaceLightIllum, 756, ACTIVE, NONE, 1, 
;   			SPACE, -1, NORMAL, NUMBERS, STD, 20, 36, 0, 6
;   		      "Lighting System",      165,  2, 0, 1, 0, 3, LIGHTING-SYSTEM,  -1, 13584, 32084, 0, ""
;   		      "Power",                 50,  2, 1, 1, 0, 3, LIGHTING-KW,      -1, 62015, 32084, 0, "Maximum amount of power consumed by the overhead lighting subsystem"
;   		      "Number of Luminaires",  65,  2, 0, 1, 0, 3, NO-OF-LUMINAIRES, -1, 62019,     0, 0, "No. of luminaires in the lighting subsystem, of the type defined by the chosen Lighting System"
;   		      "Illuminance",           65,  2, 1, 1, 0, 3, ELEC-ILLUMINANCE, -1,  3005,     0, 0, "Desired average illuminance from each of the lighting subsystems"
;   		      "Ceil to Lum Distance",  70,  2, 1, 1, 0, 3, CEIL-TO-LUM-DIS,  -1, 62017,     0, 0, "Distance from the ceiling to the center plane of the luminaires"
;   		      "Schedule",             170,  2, 0, 1, 0, 3, LIGHTING-SCHEDUL, -1, 62013,     0, 0, "A fractional schedule that adjusts the lighting subsystem's power consumption each hour"

   SPREAD, SpaceLightLum, 736, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 4
   		      "Lighting System",      160, 32, 0, 0, 0, 3, LIGHTING-SYSTEM,  -1, 13584, 32084, 0, ""
   		      "Power Input",           78,  1, 1, 0, 0, 3, LIGHTING-SYSTEM,  -1, 12311, 32084, 1, LIGHTING-SYSTEM, 0, TOT-POWER-INPUT,  -1, ""
   		      "Configuration",        140, 32, 0, 0, 0, 3, LIGHTING-SYSTEM,  -1, 13583, 32084, 1, LIGHTING-SYSTEM, 0, LUMINAIRE-CONFIG, -1, ""
   		      "Luminaire Type",       160, 32, 0, 0, 0, 3, LIGHTING-SYSTEM,  -1, 19032, 32084, 1, LIGHTING-SYSTEM, 0, LUMINAIRE-TYPE,   -1, ""

   SPREAD, SpaceLightLamp, 746, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 4
   		      "Lighting System",      145, 32, 0, 0, 0, 3, LIGHTING-SYSTEM,  -1, 13584, 32084, 0, ""
   		      "Lamp Type",            145, 32, 0, 0, 0, 3, LIGHTING-SYSTEM,  -1, 12295, 32084, 1, LIGHTING-SYSTEM, 0, LAMP-TYPE,       -1, ""
   		      "Lamp Lumens",          100,  1, 1, 0, 0, 3, LIGHTING-SYSTEM,  -1, 12316, 32084, 1, LIGHTING-SYSTEM, 0, TOT-LAMP-LUMENS, -1, ""
   		      "Ballast Type",         145, 32, 0, 0, 0, 3, LIGHTING-SYSTEM,  -1, 19047, 32084, 1, LIGHTING-SYSTEM, 0, BALLAST-TYPE,    -1, ""

; AFR 6/24/09 - display for non-LEED   			
   SPREAD, SpaceOccTypeSpread, 702, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 3                     ;    ItmHlp  TpcHlp
               "Occupancy Type",         164, 80, 1, 1,  1, 1, C-OCC-TYPE,         -1,      0,     0,  0, "The occupancy of this activity area"
               "Area",                    75,  2, 1, 1,  1, 1, C-SUB-AREA,         -1,      0,     0,  0, "The floor area of this activity area"
               "Tailored Vent",          100,  2, 1, 1,  1, 1, C-TLD-VENT-CFM/A,   -1,      0,     0,  0, "The tailored ventilation rate for this activity area"
; AFR 5/14/09 - copied "Tailored Vent" from the compliance tab.

; AFR 6/24/09 - display for LEED               
   SPREAD, Space901OccTypeSpread, 698, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 2                     ;    ItmHlp  TpcHlp
               "Occupancy Type",         164, 80, 1, 1,  1, 1, C-901-OCC-TYPE,     -1,      0,     0,  0, "ASHRAE activity area description"
               "Area",                    75,  2, 1, 1,  1, 1, C-SUB-AREA,         -1,      0,     0,  0, "The floor area of this activity area"

   SPREAD, SpaceCompLtgSpread, 704, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 25, 20, 2, 5                     ;    ItmHlp  TpcHlp
               "Occupancy Type",         158, 80, 1, 0,  1, 1, C-OCC-TYPE,         -1,      0,     0,  0, "The occupancy of this activity area"
               "Area",                    70,  1, 1, 0,  1, 1, C-SUB-AREA,         -1,      0,     0,  0, "The floor area of this activity area"
               "Lighting",               105,  2, 1, 1,  1, 1, C-SUB-LTG-W/AREA,   -1,      0,     0,  0, "The general lighting power density for this activity area"
               "Task Light",             105,  2, 1, 1,  1, 1, C-SUB-TSK-LT-KW,    -1,      0,     0,  0, "The total connected task lighting power for this activity area"
               "Task Light",             115,  2, 1, 1,  1, 1, C-SUB-TSK-LT-W/A,   -1,      0,     0,  0, "The task lighting power density for this activity area"

   SPREAD, SpaceCompTailoredSpread, 705, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 25, 36, 2, 5                     ;    ItmHlp  TpcHlp
               "Occupancy Type",         158, 80, 1, 0,  1, 1, C-OCC-TYPE,         -1,      0,     0,  0, "The occupancy of this activity area"
               "Area",                    70,  1, 1, 0,  1, 1, C-SUB-AREA,         -1,      0,     0,  0, "The floor area of this activity area"
               "Tailored Vent",          100,  2, 1, 1,  1, 1, C-TLD-VENT-CFM/A,   -1,      0,     0,  0, "The tailored ventilation rate for this activity area"
               "Tailored Lighting",      100,  2, 1, 1,  1, 1, C-TLD-LTG-W/AREA,   -1,      0,     0,  0, "The tailored lighting allowance for this space"
               "Lighting Cntrl Credits", 100,  2, 1, 1,  1, 1, C-LTG-CNTRL-CRED,   -1,      0,     0,  0, "The lighting control credits for this space"

; SAC 7/25/06 - removed per KJM e-mail of 6/27/06
;   SPREAD, SpaceCompSourceSpread, 706, ACTIVE, NONE, 1, 
;   			SPACE, -1, NORMAL, NUMBERS, STD, 25, 20, 2, 6                     ;    ItmHlp  TpcHlp
;               "Occupancy Type",         158, 80, 1, 0,  1, 1, C-OCC-TYPE,         -1,      0,     0,  0, "The occupancy of this activity area"
;               "Area",                    70,  1, 1, 0,  1, 1, C-SUB-AREA,         -1,      0,     0,  0, "The floor area of this activity area"
;               "Process",                100,  2, 1, 1,  1, 1, C-SUB-SRC-BTUH,     -1,      0,     0,  0, "The process load for this activity area in Btuh"
;               "Process",                 90,  2, 1, 1,  1, 1, C-SUB-SRC-KW,       -1,      0,     0,  0, "The process load for this activity area in kW"
;               "Sensible Frac",           98,  3, 1, 1,  1, 1, C-SUB-SRC-SENS,     -1,      0,     0,  0, "The fraction of process loads that are sensible"
;               "Latent Frac",             88,  3, 1, 1,  1, 1, C-SUB-SRC-LATENT,   -1,      0,     0,  0, "The fraction of process loads that are latent"

   SPREAD, SpaceDiscreteSpread, 706, ACTIVE, NONE, 1, 
   			SPACE, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 4     ;   ItmHlp  TpcHlp
                 "Input Pwr System 1",  65,  3, 1, 1,  1, 3, DISCRETE-POWER1 , -1,  12071,  3002,  0, "Lighting input power fraction for control system 1"
                 "Output Illum 1",      65,  3, 1, 1,  1, 3, DISCRETE-LIGHT1 , -1,  12072,  3002,  0, "Lighting illumiance output fraction for control system 1"
                 "Input Pwr System 2",  65,  3, 1, 1,  1, 3, DISCRETE-POWER2 , -1,    727,  3002,  0, "Lighting input power fraction for control system 2"
                 "Output Illum 2",      65,  3, 1, 1,  1, 3, DISCRETE-LIGHT2 , -1,  12073,  3002,  0, "Lighting illumiance output fraction for control system 2"

   ;*****   Window Spreadsheets   *****

   SPREAD, WinStrSpread, 646, ACTIVE, NONE, 1,
            WINDOW, -1, NORMAL, NUMBERS, STD, 20, 20, 0, 1
               "Window Layers",        209,  2, 0, 1, 0, 3, WINDOW-LAYERS, -1, 61032, 32012, 0, ""

   SPREAD, SkylightTRSpread, 647, ACTIVE, NONE, 1, 
   			WINDOW, -1, NORMAL, NUMBERS, STD, 20, 36, 0, 2     ;   ItmHlp  TpcHlp
                 "Angle",  55,  4, 1, 1,  1, 3, SKY-TRANS-ANG  , -1,  12071,  3002,  0, "Angle of direct solar incidence"
        "Transmiss Mult",  62,  4, 1, 1,  1, 3, SKY-TRANS-MULT , -1,    727,  3002,  0, "Multiplier on zero degree direct transmission"

            
   ;*****   Polygon Spreadsheet   *****

   SPREAD, PolySpread, 576, ACTIVE, PAIR, 1, 
   			POLYGON, -1, TRANSPOSE, XYZ, STD, 100, 20, 0, 120
                  "Vertex 1",   80,  2, 1, 1, 0, 3, V1,   -1, 31033, 31030, 0, ""
                  "Vertex 2",   80,  2, 1, 1, 0, 3, V2,   -1, 31033, 31030, 0, ""
                  "Vertex 3",   80,  2, 1, 1, 0, 3, V3,   -1, 31033, 31030, 0, ""
                  "Vertex 4",   80,  2, 1, 1, 0, 3, V4,   -1, 31033, 31030, 0, ""
                  "Vertex 5",   80,  2, 1, 1, 0, 3, V5,   -1, 31033, 31030, 0, ""
                  "Vertex 6",   80,  2, 1, 1, 0, 3, V6,   -1, 31033, 31030, 0, ""
                  "Vertex 7",   80,  2, 1, 1, 0, 3, V7,   -1, 31033, 31030, 0, ""
                  "Vertex 8",   80,  2, 1, 1, 0, 3, V8,   -1, 31033, 31030, 0, ""
                  "Vertex 9",   80,  2, 1, 1, 0, 3, V9,   -1, 31033, 31030, 0, ""
                  "Vertex 10",  80,  2, 1, 1, 0, 3, V10,  -1, 31033, 31030, 0, ""
                  "Vertex 11",  80,  2, 1, 1, 0, 3, V11,  -1, 31033, 31030, 0, ""
                  "Vertex 12",  80,  2, 1, 1, 0, 3, V12,  -1, 31033, 31030, 0, ""
                  "Vertex 13",  80,  2, 1, 1, 0, 3, V13,  -1, 31033, 31030, 0, ""
                  "Vertex 14",  80,  2, 1, 1, 0, 3, V14,  -1, 31033, 31030, 0, ""
                  "Vertex 15",  80,  2, 1, 1, 0, 3, V15,  -1, 31033, 31030, 0, ""
                  "Vertex 16",  80,  2, 1, 1, 0, 3, V16,  -1, 31033, 31030, 0, ""
                  "Vertex 17",  80,  2, 1, 1, 0, 3, V17,  -1, 31033, 31030, 0, ""
                  "Vertex 18",  80,  2, 1, 1, 0, 3, V18,  -1, 31033, 31030, 0, ""
                  "Vertex 19",  80,  2, 1, 1, 0, 3, V19,  -1, 31033, 31030, 0, ""
                  "Vertex 20",  80,  2, 1, 1, 0, 3, V20,  -1, 31033, 31030, 0, ""
                  "Vertex 21",  80,  2, 1, 1, 0, 3, V21,  -1, 31033, 31030, 0, ""
                  "Vertex 22",  80,  2, 1, 1, 0, 3, V22,  -1, 31033, 31030, 0, ""
                  "Vertex 23",  80,  2, 1, 1, 0, 3, V23,  -1, 31033, 31030, 0, ""
                  "Vertex 24",  80,  2, 1, 1, 0, 3, V24,  -1, 31033, 31030, 0, ""
                  "Vertex 25",  80,  2, 1, 1, 0, 3, V25,  -1, 31033, 31030, 0, ""
                  "Vertex 26",  80,  2, 1, 1, 0, 3, V26,  -1, 31033, 31030, 0, ""
                  "Vertex 27",  80,  2, 1, 1, 0, 3, V27,  -1, 31033, 31030, 0, ""
                  "Vertex 28",  80,  2, 1, 1, 0, 3, V28,  -1, 31033, 31030, 0, ""
                  "Vertex 29",  80,  2, 1, 1, 0, 3, V29,  -1, 31033, 31030, 0, ""
                  "Vertex 30",  80,  2, 1, 1, 0, 3, V30,  -1, 31033, 31030, 0, ""
                  "Vertex 31",  80,  2, 1, 1, 0, 3, V31,  -1, 31033, 31030, 0, ""
                  "Vertex 32",  80,  2, 1, 1, 0, 3, V32,  -1, 31033, 31030, 0, ""
                  "Vertex 33",  80,  2, 1, 1, 0, 3, V33,  -1, 31033, 31030, 0, ""
                  "Vertex 34",  80,  2, 1, 1, 0, 3, V34,  -1, 31033, 31030, 0, ""
                  "Vertex 35",  80,  2, 1, 1, 0, 3, V35,  -1, 31033, 31030, 0, ""
                  "Vertex 36",  80,  2, 1, 1, 0, 3, V36,  -1, 31033, 31030, 0, ""
                  "Vertex 37",  80,  2, 1, 1, 0, 3, V37,  -1, 31033, 31030, 0, ""
                  "Vertex 38",  80,  2, 1, 1, 0, 3, V38,  -1, 31033, 31030, 0, ""
                  "Vertex 39",  80,  2, 1, 1, 0, 3, V39,  -1, 31033, 31030, 0, ""
                  "Vertex 40",  80,  2, 1, 1, 0, 3, V40,  -1, 31033, 31030, 0, ""
                  "Vertex 41",  80,  2, 1, 1, 0, 3, V41,  -1, 31033, 31030, 0, ""
                  "Vertex 42",  80,  2, 1, 1, 0, 3, V42,  -1, 31033, 31030, 0, ""
                  "Vertex 43",  80,  2, 1, 1, 0, 3, V43,  -1, 31033, 31030, 0, ""
                  "Vertex 44",  80,  2, 1, 1, 0, 3, V44,  -1, 31033, 31030, 0, ""
                  "Vertex 45",  80,  2, 1, 1, 0, 3, V45,  -1, 31033, 31030, 0, ""
                  "Vertex 46",  80,  2, 1, 1, 0, 3, V46,  -1, 31033, 31030, 0, ""
                  "Vertex 47",  80,  2, 1, 1, 0, 3, V47,  -1, 31033, 31030, 0, ""
                  "Vertex 48",  80,  2, 1, 1, 0, 3, V48,  -1, 31033, 31030, 0, ""
                  "Vertex 49",  80,  2, 1, 1, 0, 3, V49,  -1, 31033, 31030, 0, ""
                  "Vertex 50",  80,  2, 1, 1, 0, 3, V50,  -1, 31033, 31030, 0, ""
                  "Vertex 51",  80,  2, 1, 1, 0, 3, V51,  -1, 31033, 31030, 0, ""
                  "Vertex 52",  80,  2, 1, 1, 0, 3, V52,  -1, 31033, 31030, 0, ""
                  "Vertex 53",  80,  2, 1, 1, 0, 3, V53,  -1, 31033, 31030, 0, ""
                  "Vertex 54",  80,  2, 1, 1, 0, 3, V54,  -1, 31033, 31030, 0, ""
                  "Vertex 55",  80,  2, 1, 1, 0, 3, V55,  -1, 31033, 31030, 0, ""
                  "Vertex 56",  80,  2, 1, 1, 0, 3, V56,  -1, 31033, 31030, 0, ""
                  "Vertex 57",  80,  2, 1, 1, 0, 3, V57,  -1, 31033, 31030, 0, ""
                  "Vertex 58",  80,  2, 1, 1, 0, 3, V58,  -1, 31033, 31030, 0, ""
                  "Vertex 59",  80,  2, 1, 1, 0, 3, V59,  -1, 31033, 31030, 0, ""
                  "Vertex 60",  80,  2, 1, 1, 0, 3, V60,  -1, 31033, 31030, 0, ""
                  "Vertex 61",  80,  2, 1, 1, 0, 3, V61,  -1, 31033, 31030, 0, ""
                  "Vertex 62",  80,  2, 1, 1, 0, 3, V62,  -1, 31033, 31030, 0, ""
                  "Vertex 63",  80,  2, 1, 1, 0, 3, V63,  -1, 31033, 31030, 0, ""
                  "Vertex 64",  80,  2, 1, 1, 0, 3, V64,  -1, 31033, 31030, 0, ""
                  "Vertex 65",  80,  2, 1, 1, 0, 3, V65,  -1, 31033, 31030, 0, ""
                  "Vertex 66",  80,  2, 1, 1, 0, 3, V66,  -1, 31033, 31030, 0, ""
                  "Vertex 67",  80,  2, 1, 1, 0, 3, V67,  -1, 31033, 31030, 0, ""
                  "Vertex 68",  80,  2, 1, 1, 0, 3, V68,  -1, 31033, 31030, 0, ""
                  "Vertex 69",  80,  2, 1, 1, 0, 3, V69,  -1, 31033, 31030, 0, ""
                  "Vertex 70",  80,  2, 1, 1, 0, 3, V70,  -1, 31033, 31030, 0, ""
                  "Vertex 71",  80,  2, 1, 1, 0, 3, V71,  -1, 31033, 31030, 0, ""
                  "Vertex 72",  80,  2, 1, 1, 0, 3, V72,  -1, 31033, 31030, 0, ""
                  "Vertex 73",  80,  2, 1, 1, 0, 3, V73,  -1, 31033, 31030, 0, ""
                  "Vertex 74",  80,  2, 1, 1, 0, 3, V74,  -1, 31033, 31030, 0, ""
                  "Vertex 75",  80,  2, 1, 1, 0, 3, V75,  -1, 31033, 31030, 0, ""
                  "Vertex 76",  80,  2, 1, 1, 0, 3, V76,  -1, 31033, 31030, 0, ""
                  "Vertex 77",  80,  2, 1, 1, 0, 3, V77,  -1, 31033, 31030, 0, ""
                  "Vertex 78",  80,  2, 1, 1, 0, 3, V78,  -1, 31033, 31030, 0, ""
                  "Vertex 79",  80,  2, 1, 1, 0, 3, V79,  -1, 31033, 31030, 0, ""
                  "Vertex 80",  80,  2, 1, 1, 0, 3, V80,  -1, 31033, 31030, 0, ""
                  "Vertex 81",  80,  2, 1, 1, 0, 3, V81,  -1, 31033, 31030, 0, ""
                  "Vertex 82",  80,  2, 1, 1, 0, 3, V82,  -1, 31033, 31030, 0, ""
                  "Vertex 83",  80,  2, 1, 1, 0, 3, V83,  -1, 31033, 31030, 0, ""
                  "Vertex 84",  80,  2, 1, 1, 0, 3, V84,  -1, 31033, 31030, 0, ""
                  "Vertex 85",  80,  2, 1, 1, 0, 3, V85,  -1, 31033, 31030, 0, ""
                  "Vertex 86",  80,  2, 1, 1, 0, 3, V86,  -1, 31033, 31030, 0, ""
                  "Vertex 87",  80,  2, 1, 1, 0, 3, V87,  -1, 31033, 31030, 0, ""
                  "Vertex 88",  80,  2, 1, 1, 0, 3, V88,  -1, 31033, 31030, 0, ""
                  "Vertex 89",  80,  2, 1, 1, 0, 3, V89,  -1, 31033, 31030, 0, ""
                  "Vertex 90",  80,  2, 1, 1, 0, 3, V90,  -1, 31033, 31030, 0, ""
                  "Vertex 91",  80,  2, 1, 1, 0, 3, V91,  -1, 31033, 31030, 0, ""
                  "Vertex 92",  80,  2, 1, 1, 0, 3, V92,  -1, 31033, 31030, 0, ""
                  "Vertex 93",  80,  2, 1, 1, 0, 3, V93,  -1, 31033, 31030, 0, ""
                  "Vertex 94",  80,  2, 1, 1, 0, 3, V94,  -1, 31033, 31030, 0, ""
                  "Vertex 95",  80,  2, 1, 1, 0, 3, V95,  -1, 31033, 31030, 0, ""
                  "Vertex 96",  80,  2, 1, 1, 0, 3, V96,  -1, 31033, 31030, 0, ""
                  "Vertex 97",  80,  2, 1, 1, 0, 3, V97,  -1, 31033, 31030, 0, ""
                  "Vertex 98",  80,  2, 1, 1, 0, 3, V98,  -1, 31033, 31030, 0, ""
                  "Vertex 99",  80,  2, 1, 1, 0, 3, V99,  -1, 31033, 31030, 0, ""
                  "Vertex 100", 80,  2, 1, 1, 0, 3, V100, -1, 31033, 31030, 0, ""
                  "Vertex 101", 80,  2, 1, 1, 0, 3, V101, -1, 31033, 31030, 0, ""
                  "Vertex 102", 80,  2, 1, 1, 0, 3, V102, -1, 31033, 31030, 0, ""
                  "Vertex 103", 80,  2, 1, 1, 0, 3, V103, -1, 31033, 31030, 0, ""
                  "Vertex 104", 80,  2, 1, 1, 0, 3, V104, -1, 31033, 31030, 0, ""
                  "Vertex 105", 80,  2, 1, 1, 0, 3, V105, -1, 31033, 31030, 0, ""
                  "Vertex 106", 80,  2, 1, 1, 0, 3, V106, -1, 31033, 31030, 0, ""
                  "Vertex 107", 80,  2, 1, 1, 0, 3, V107, -1, 31033, 31030, 0, ""
                  "Vertex 108", 80,  2, 1, 1, 0, 3, V108, -1, 31033, 31030, 0, ""
                  "Vertex 109", 80,  2, 1, 1, 0, 3, V109, -1, 31033, 31030, 0, ""
                  "Vertex 110", 80,  2, 1, 1, 0, 3, V110, -1, 31033, 31030, 0, ""
                  "Vertex 111", 80,  2, 1, 1, 0, 3, V111, -1, 31033, 31030, 0, ""
                  "Vertex 112", 80,  2, 1, 1, 0, 3, V112, -1, 31033, 31030, 0, ""
                  "Vertex 113", 80,  2, 1, 1, 0, 3, V113, -1, 31033, 31030, 0, ""
                  "Vertex 114", 80,  2, 1, 1, 0, 3, V114, -1, 31033, 31030, 0, ""
                  "Vertex 115", 80,  2, 1, 1, 0, 3, V115, -1, 31033, 31030, 0, ""
                  "Vertex 116", 80,  2, 1, 1, 0, 3, V116, -1, 31033, 31030, 0, ""
                  "Vertex 117", 80,  2, 1, 1, 0, 3, V117, -1, 31033, 31030, 0, ""
                  "Vertex 118", 80,  2, 1, 1, 0, 3, V118, -1, 31033, 31030, 0, ""
                  "Vertex 119", 80,  2, 1, 1, 0, 3, V119, -1, 31033, 31030, 0, ""
                  "Vertex 120", 80,  2, 1, 1, 0, 3, V120, -1, 31033, 31030, 0, ""
                                                 
                                                 
   ;*****   Constructions Spreadsheets   *****   
                                                 
   SPREAD, ConsSpread, 596, ACTIVE, NONE, 1, 
   			LAYERS, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 6
               "Material Name",  184, 32, 1, 0, 0, 3, MATERIAL,   -1, 13124, 13124, 0, ""
               "Thickness",       75,  3, 1, 0, 0, 3, THICKNESS,  -1, 13125, 13125, 0, ""
               "Conductivity",    90,  4, 1, 0, 0, 3, MATERIAL,   -1, 13126, 13126, 1, MATERIAL, 0, CONDUCTIVITY,  -1, ""
               "Density",         70,  2, 1, 0, 0, 3, MATERIAL,   -1, 13127, 13127, 1, MATERIAL, 0, DENSITY,       -1, ""
               "Spec. Heat",      85,  3, 1, 0, 0, 3, MATERIAL,   -1, 13128, 13128, 1, MATERIAL, 0, SPECIFIC-HEAT, -1, ""
               "R-Value",         90,  3, 1, 0, 0, 3, MATERIAL,   -1, 13129, 13129, 1, MATERIAL, 0, RESISTANCE,    -1, ""

            
   ;*****   Layers Spreadsheets   *****

;   SPREAD, LayersSpread, 606, ACTIVE, PAIR, 1, 
; SAC 11/5/00 - Revised spreadsheet configuration to replace PAIR classification with NONE - enable THICKNESS defaulting
   SPREAD, LayersSpread, 606, ACTIVE, NONE, 1, 
   			LAYERS, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 6
               "Material Name",  199,  0, 1, 1, 0, 3, MATERIAL,   -1, 13124, 13124, 0, ""
               "Thickness",       75,  3, 1, 1, 0, 3, THICKNESS,  -1, 13125, 13125, 0, ""
               "Conductivity",    90,  4, 1, 0, 0, 3, MATERIAL,   -1, 13126, 13126, 1, MATERIAL, 0, CONDUCTIVITY,   -1, ""
               "Density",         70,  2, 1, 0, 0, 3, MATERIAL,   -1, 13127, 13127, 1, MATERIAL, 0, DENSITY,        -1, ""
               "Spec. Heat",      85,  3, 1, 0, 0, 3, MATERIAL,   -1, 13128, 13128, 1, MATERIAL, 0, SPECIFIC-HEAT,  -1, ""
               "R-Value",         90,  3, 1, 0, 0, 3, MATERIAL,   -1, 13129, 13129, 1, MATERIAL, 0, RESISTANCE,     -1, ""


   ;*****   Glass Type Spreadsheets   *****

   SPREAD, GlassSpread, 616, ACTIVE, SINGLE_NO_FILL, 1,
   			GLASS-TYPE-CODE, -1, NORMAL, NUMBERS, STD, 25, 20, 1, 6
               "Glass",          82,  0, 1, 0, 0, 3,     PANES-ID,      -1, 61016, 0, 0, ""
               "Width",          55,  3, 1, 0, 0, 3,  PANES-THICK,      -1, 61017, 0, 0, ""
               "Thrm Inf Trans", 90,  3, 1, 0, 0, 3,    PANES-TIR,      -1, 61018, 0, 0, ""
               "Front Emis.",    80,  3, 1, 0, 0, 3, PANES-EMIS-F,      -1, 61019, 0, 0, ""
               "Back Emis.",     80,  3, 1, 0, 0, 3, PANES-EMIS-B,      -1, 61020, 0, 0, ""
               "Conductance",    90,  1, 1, 0, 0, 3,   PANES-COND,      -1, 61021, 0, 0, ""

   SPREAD, GlassGapSpread, 626, ACTIVE, PAIR, 1,
   			GLASS-TYPE-CODE, -1, NORMAL, NUMBERS, STD, 25, 20, 1, 10
               "Gas",            60, 32, 1, 0, 0, 3,   GAPS-FILL,       -1, 61022, 0, 0, ""
               "Width",          55,  3, 1, 0, 0, 3,  GAPS-THICK,       -1, 61023, 0, 0, ""
               "Conductivity",   85,  3, 1, 0, 0, 3,   GAPS-COND,       -1, 61024, 0, 0, ""
               "dConductivity",  90,  3, 1, 0, 0, 3,  GAPS-DCOND,       -1, 61025, 0, 0, ""
               "Viscosity",      75,  3, 1, 0, 0, 3,   GAPS-VISC,       -1, 61026, 0, 0, ""
               "dViscosity",     80,  3, 1, 0, 0, 3,  GAPS-DVISC,       -1, 61027, 0, 0, ""
               "Density",        65,  3, 1, 0, 0, 3,   GAPS-DENS,       -1, 61028, 0, 0, ""
               "dDensity",       70,  3, 1, 0, 0, 3,  GAPS-DDENS,       -1, 61029, 0, 0, ""
               "Prandtl num",    80,  3, 1, 0, 0, 3,     GAPS-PR,       -1, 61030, 0, 0, ""
               "dPrandtl num",   85,  3, 1, 0, 0, 3,    GAPS-DPR,       -1, 61031, 0, 0, ""

   SPREAD, GTCSpread, 636, ACTIVE, TRIPLET, 1,
            GLASS-TYPE-CODE, -1, NORMAL, ANGLE, STD, 55, 20, 0, 7
               "Solar Trans",    85, 2, 1, 0, 0, 3,  TSOL,     -1, 13145, 0, 0, "Solar transmittance of the selected glass type code"
               "Visible Trans",  88, 2, 1, 0, 0, 3,  TVIS,     -1, 13146, 0, 0, "Visible transmittance of the selected glass type code"
               "Sol Abs 1",      72, 2, 1, 0, 0, 3, ABS-1,     -1, 61034, 0, 0, ""
               "Sol Abs 2",      72, 2, 1, 0, 0, 3, ABS-2,     -1, 61035, 0, 0, ""
               "Sol Abs 3",      72, 2, 1, 0, 0, 3, ABS-3,     -1, 61036, 0, 0, ""
               "Sol Abs 4",      72, 2, 1, 0, 0, 3, ABS-4,     -1, 61037, 0, 0, ""
               "Sol Abs 5",      72, 2, 1, 0, 0, 3, ABS-5,     -1, 61038, 0, 0, ""


   ;*****   System Spreadsheets   *****

   SPREAD, SysPipeTypeSpread, 703, ACTIVE, NONE, 1, 
   			SYSTEM, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 2               ;    ItmHlp  TpcHlp
               "Type of Piping",      168, 32, 1, 1,  1, 1, C-PIPE-TYPE,       -1,      0,     0,  0, "The type of pipe"
               "Insulation R-Value",   75,  2, 1, 1,  1, 1, C-PIPE-INS-RVAL,   -1,      0,     0,  0, "The required minimum R-Value for the type of pipe selected"

; SAC 6/30/03 - Added spreadsheets to support new SBD cool/heat duct losses analysis
   SPREAD, SysSBDCoolDuctSpread, 707, ACTIVE, NONE, 1, 
   			SYSTEM, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 7               ;    ItmHlp  TpcHlp
               "Cooling Duct Type",  150, 32, 1, 1,  1, 4, C-SUPPLY-DUCT,    -1,      0,      0,  0, ""
               "Height",              50,  2, 1, 1,  1, 4, C-SUPPLY-HT,      -1,      0,      0,  0, ""
               "Width",               50,  2, 1, 1,  1, 4, C-SUPPLY-WD,      -1,      0,      0,  0, ""
               "Diameter",            65,  2, 1, 1,  1, 4, C-SUPPLY-DIAM,    -1,      0,      0,  0, ""
               "Circumference",      100,  2, 1, 1,  1, 4, C-SUPPLY-CIRCUM,  -1,      0,      0,  0, ""
               "Length",              52,  2, 1, 1,  1, 4, C-SUPPLY-LENGTH,  -1,      0,      0,  0, ""
               "Insul R-Value",       95,  2, 1, 1,  1, 4, C-SUPPLY-RVAL,    -1,      0,      0,  0, ""

   SPREAD, SysSBDHeatDuctSpread, 708, ACTIVE, NONE, 1, 
   			SYSTEM, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 7               ;    ItmHlp  TpcHlp
               "Heating Duct Type",  150, 32, 1, 1,  1, 4, C-HSUPPLY-DUCT,   -1,      0,      0,  0, ""
               "Height",              50,  2, 1, 1,  1, 4, C-HSUPPLY-HT,     -1,      0,      0,  0, ""
               "Width",               50,  2, 1, 1,  1, 4, C-HSUPPLY-WD,     -1,      0,      0,  0, ""
               "Diameter",            65,  2, 1, 1,  1, 4, C-HSUPPLY-DIAM,   -1,      0,      0,  0, ""
               "Circumference",      100,  2, 1, 1,  1, 4, C-HSUPPLY-CIRCUM, -1,      0,      0,  0, ""
               "Length",              52,  2, 1, 1,  1, 4, C-HSUPPLY-LENGTH, -1,      0,      0,  0, ""
               "Insul R-Value",       95,  2, 1, 1,  1, 4, C-HSUPPLY-RVAL,   -1,      0,      0,  0, ""

; SAC 1/18/06 - Added new spreads for T-24 2005 duct inputs
   SPREAD, SysSupplyDuctSpread, 711, ACTIVE, NONE, 1, 
   			SYSTEM, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 3               ;    ItmHlp  TpcHlp
               "Zone",               105, 32, 0, 1,  1, 1, C-SUP-DUCT-ZONE,  -1,      0,      0,  0, ""
               "Zone Type",           80, 32, 0, 1,  1, 1, C-SDUCT-SPC-TYPE, -1,      0,      0,  0, ""
               "Area Fraction",       55,  2, 0, 1,  1, 1, C-SUP-DUCT-FRAC,  -1,      0,      0,  0, ""

   SPREAD, SysReturnDuctSpread, 712, ACTIVE, NONE, 1, 
   			SYSTEM, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 3               ;    ItmHlp  TpcHlp
               "Zone",               105, 32, 0, 1,  1, 1, C-RET-DUCT-ZONE,  -1,      0,      0,  0, ""
               "Zone Type",           80, 32, 0, 1,  1, 1, C-RDUCT-SPC-TYPE, -1,      0,      0,  0, ""
               "Area Fraction",       55,  2, 0, 1,  1, 1, C-RET-DUCT-FRAC,  -1,      0,      0,  0, ""


   ;*****   Circulation Loop Spreadsheets   *****

   SPREAD, CircLoopProcessSpread, 6400, ACTIVE, NONE, 1, 
; SAC 11/30/10 - DOE-2.3 mods
            CIRCULATION-LOOP, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 6
				   "Load",              80,  3, 1, 1, 0, 3, PROCESS-LOAD,          -1,   992,     0, 0, "Specifies a process load attached directly to the loop"
				   "Flow",              80,  3, 1, 1, 0, 3, PROCESS-FLOW,          -1, 12868,     0, 0, "Peak Process Load flow rate"
                                   "Head",              80,  1, 1, 1, 0, 3, PROCESS-HEAD,          -1,     0,     0, 0, "Pressure drop of the loop fluid through the process load"
				   "Load Schedule",    170,  0, 1, 1, 0, 3, PROCESS-SCH,           -1, 12867,     0, 0, "Schedule of multipliers applied to the Process Load"
				   "Load Delta T",      90,  1, 1, 1, 0, 3, PROCESS-LOAD-DT,       -1, 12869,     0, 0, "Delta T of the process load fluid (used to calculate Process Flow Rate, sign is irrelevant)"
				   "Hot/Cold Mixed T", 100,  1, 1, 1, 0, 3, PROCESS-T,             -1, 19216,     0, 0, "Hot/Cold mixed temperature of the DHW process load"

; SAC 7/1/03 - Added spreadsheets to support new SBD supply/return piping losses analysis
   SPREAD, CircLoopSBDSupplyPipingSpread, 709, ACTIVE, NONE, 1, 
   			CIRCULATION-LOOP, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 4               ;    ItmHlp  TpcHlp
               "Pipe Diameter",       70, 32, 1, 1,  1, 4, C-SUPPLY-SIZE,      -1,      0,      0,  0, ""
               "Length",              50,  1, 1, 1,  1, 4, C-SUPPLY-LENGTH,    -1,      0,      0,  0, ""
               "Insulation Type",    120, 32, 1, 1,  1, 4, C-SUPPLY-INS-TYPE,  -1,      0,      0,  0, ""
               "Thickns",             55,  2, 1, 1,  1, 4, C-SUPPLY-INS-THK,   -1,      0,      0,  0, ""

   SPREAD, CircLoopSBDReturnPipingSpread, 710, ACTIVE, NONE, 1, 
   			CIRCULATION-LOOP, -1, NORMAL, NUMBERS, STD, 25, 36, 0, 4               ;    ItmHlp  TpcHlp
               "Pipe Diameter",       70, 32, 1, 1,  1, 4, C-RETURN-SIZE,      -1,      0,      0,  0, ""
               "Length",              50,  1, 1, 1,  1, 4, C-RETURN-LENGTH,    -1,      0,      0,  0, ""
               "Insulation Type",    120, 32, 1, 1,  1, 4, C-RETURN-INS-TYPE,  -1,      0,      0,  0, ""
               "Thickns",             55,  2, 1, 1,  1, 4, C-RETURN-INS-THK,   -1,      0,      0,  0, ""


   ;*****   Ground Loop HX Spreadsheets   *****

; SDG 11/27/2011 – Spreadsheets no longer applicable

   ;*****   G Functions Spreadsheet   *****

; JJH 1/17/06 - GSHP mods
   SPREAD, GFuncSpread, 1480, ACTIVE, NONE, 1, 
   			G-FUNCTIONS, -1, TRANSPOSE, GFUNC, STD, 125, 36, 0, 9
                  "G Function Values",    80,  5, 1, 1, 0, 3,    G-FUNC-VALUES,   -1, 0, 0, 0, ""
                  "Space/Depth = 0.02",   80,  5, 1, 0, 0, 3, SPACE/DEPTH-0.02,   -1, 0, 0, 0, ""
                  "Space/Depth = 0.03",   80,  5, 1, 0, 0, 3, SPACE/DEPTH-0.03,   -1, 0, 0, 0, ""
                  "Space/Depth = 0.05",   80,  5, 1, 0, 0, 3, SPACE/DEPTH-0.05,   -1, 0, 0, 0, ""
                  "Space/Depth = 0.10",   80,  5, 1, 0, 0, 3, SPACE/DEPTH-0.10,   -1, 0, 0, 0, ""
                  "Space/Depth = 0.15",   80,  5, 1, 0, 0, 3, SPACE/DEPTH-0.15,   -1, 0, 0, 0, ""
                  "Space/Depth = 0.20",   80,  5, 1, 0, 0, 3, SPACE/DEPTH-0.20,   -1, 0, 0, 0, ""
                  "Space/Depth = 0.30",   80,  5, 1, 0, 0, 3, SPACE/DEPTH-0.30,   -1, 0, 0, 0, ""
                  "Space/Depth = 0.50",   80,  5, 1, 0, 0, 3, SPACE/DEPTH-0.50,   -1, 0, 0, 0, ""


   ;*****   Steam Meter Spreadsheets   *****

; SAC 9/27/04 - Added access to existing INTERIOR-EU and new EXTERIOR-EU keywords
   SPREAD,  SteamMtrInt, 1586, ACTIVE, NONE, 1, 
			   STEAM-METER, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 3
		         "Load",          90,  2, 1, 1, 0, 3,  INTERIOR-POWER, -1, 731, 0, 0, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads "
		         "Schedule",     200,  2, 1, 1, 0, 3,    INTERIOR-SCH, -1, 730, 0, 0, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
				   "Enduse",       140,  1, 1, 1, 0, 3,     INTERIOR-EU, -1,   0, 0, 0, "Enduse to apply this energy use to"

   SPREAD,  SteamMtrExt, 1587, ACTIVE, NONE, 1, 
			   STEAM-METER, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 3
		         "Load",          90,  2, 1, 1, 0, 3,  EXTERIOR-POWER, -1, 733, 0, 0, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
		         "Schedule",     200,  2, 1, 1, 0, 3,    EXTERIOR-SCH, -1, 732, 0, 0, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
				   "Enduse",       140,  1, 1, 1, 0, 3,     EXTERIOR-EU, -1,   0, 0, 0, "Enduse to apply this energy use to"


   ;*****   CHW Meter Spreadsheets   *****

; SAC 9/27/04 - Added access to existing INTERIOR-EU and new EXTERIOR-EU keywords
   SPREAD,  CHWMtrInt, 1588, ACTIVE, NONE, 1, 
			   CHW-METER, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 3
		         "Load",          90,  2, 1, 1, 0, 3,  INTERIOR-POWER, -1, 742, 0, 0, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
		         "Schedule",     200,  2, 1, 1, 0, 3,    INTERIOR-SCH, -1, 741, 0, 0, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
				   "Enduse",       140,  1, 1, 1, 0, 3,     INTERIOR-EU, -1,   0, 0, 0, "Enduse to apply this energy use to"

   SPREAD,  CHWMtrExt, 1589, ACTIVE, NONE, 1, 
			   CHW-METER, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 3
		         "Load",          90,  2, 1, 1, 0, 3,  EXTERIOR-POWER, -1, 744, 0, 0, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
		         "Schedule",     200,  2, 1, 1, 0, 3,    EXTERIOR-SCH, -1, 743, 0, 0, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
				   "Enduse",       140,  1, 1, 1, 0, 3,     EXTERIOR-EU, -1,   0, 0, 0, "Enduse to apply this energy use to"


   ;*****   Equipment Controls Spreadsheets   *****

   ; --- Load Range 1 ---

   SPREAD,  EquipCtrl1Cl, 1556, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		                "Chiller Name",  174,  2, 0, 1, 1, 3,     CHILLERS-1, -1, 719, 0, 0, "Name of the chiller that is used to match the corresponding flow range"
		                         "Seq",   35,  0, 0, 1, 1, 3, CHILLERS-SEQ-1, -1, 720, 0, 0, "The order in which the chillers are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 1, 3,     MAX-FLOW-1, -1, 709, 0, 0, "The maximum allowable flow for the chiller"

   SPREAD,  EquipCtrl1Ht, 1557, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		                 "Boiler Name",  174,  2, 0, 1, 2, 3,     BOILERS-1, -1, 721, 0, 0, "Name of the boiler that is used to match the corresponding flow range "
		                         "Seq",   35,  0, 0, 1, 2, 3, BOILERS-SEQ-1, -1, 720, 0, 0, "The order in which the boilers are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 2, 3,    MAX-FLOW-1, -1, 709, 0, 0, "The maximum allowable flow for the boiler"

   SPREAD,  EquipCtrl1Ht2, 1558, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		         "Chiller/Heater Name",  174,  2, 0, 1, 2, 3,     CHLR/HTRS-1, -1, 717, 0, 0, "Name of the chiller/heater that is used to match the corresponding flow range"
		                         "Seq",   35,  0, 0, 1, 2, 3, CHLR/HTRS-SEQ-1, -1, 720, 0, 0, "The order in which the chiller/heaters are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 2, 3, CHLR/HTRS-MAX-1, -1, 709, 0, 0, "The maximum allowable flow for the chiller/heater"

   SPREAD,  EquipCtrl1DHW, 1559, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		              "DHW Heater Name", 174,  2, 0, 1, 3, 3,     DW-HEATERS-1, -1, 714, 0, 0, "Name of the water heater that is used to match the corresponding flow range"
		                         "Seq",   35,  0, 0, 1, 3, 3, DW-HEATERS-SEQ-1, -1, 720, 0, 0, "The order in which the water heaters are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 3, 3,       MAX-FLOW-1, -1, 709, 0, 0, "The maximum allowable flow for the water heater"

   SPREAD,  EquipCtrl1HR, 1560, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
                "Heat Reject Device",  174,  2, 0, 1, 4, 3,     HEAT-REJ-1, -1, 712, 0, 0, "Name of the heat rejector that is used to match the corresponding flow range"
                               "Seq",   35,  0, 0, 1, 4, 3, HEAT-REJ-SEQ-1, -1, 720, 0, 0, "The order in which the heat rejectors are used to satisfy the flow"
                          "Max Flow",   75,  2, 0, 1, 4, 3,     MAX-FLOW-1, -1, 710, 0, 0, "Maximum allowable flow rate that can be assigned to each heat rejector"

   SPREAD,  EquipCtrl1HR2, 1600, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		         "Ground Loop HX Name",  174,  2, 0, 1, 4, 3,         GLHX-1, -1, 717, 0, 0, "Name of the ground loop heat exchanger that is used to match the corresponding flow range"
		                         "Seq",   35,  0, 0, 1, 4, 3,     GLHX-SEQ-1, -1, 720, 0, 0, "The order in which the ground loop heat exchangers are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 4, 3,     GLHX-MAX-1, -1, 709, 0, 0, "The maximum allowable flow for the ground loop heat exchanger"

   SPREAD,  EquipCtrl1Elec, 1561, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
                    "Generator Name",  174,  2, 0, 1, 5, 3,     GENERATORS-1, -1, 714, 0, 0, "Name of the generator that is used to match the corresponding load range"
                               "Seq",   35,  0, 0, 1, 5, 3, GENERATORS-SEQ-1, -1, 720, 0, 0, "The order in which the generators are used to satisfy the load"
                          "Max Load",   75,  2, 0, 1, 5, 3,       MAX-LOAD-1, -1, 709, 0, 0, "The maximum allowable load for the generator"

   ; --- Load Range 2 ---

   SPREAD,  EquipCtrl2Cl, 1562, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		       "Chiller Name",  174,  2, 0, 1, 1, 3,     CHILLERS-2, -1, 719, 0, 0, "Name of the chiller that is used to match the corresponding flow"
		                "Seq",   35,  0, 0, 1, 1, 3, CHILLERS-SEQ-2, -1, 720, 0, 0, "The order in which the chillers are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 1, 3,     MAX-FLOW-2, -1, 709, 0, 0, "The maximum allowable flow for the chiller"

   SPREAD,  EquipCtrl2Ht, 1563, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		        "Boiler Name",  174,  2, 0, 1, 2, 3,     BOILERS-2, -1, 721, 0, 0, "Name of the boiler that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 2, 3, BOILERS-SEQ-2, -1, 720, 0, 0, "The order in which the boilers are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 2, 3,    MAX-FLOW-2, -1, 709, 0, 0, "The maximum allowable flow for the boiler"

   SPREAD,  EquipCtrl2Ht2, 1564, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		         "Chiller/Heater Name",  174,  2, 0, 1, 2, 3,     CHLR/HTRS-2, -1, 717, 0, 0, "Name of the chiller/heater that is used to match the corresponding flow range"
		                         "Seq",   35,  0, 0, 1, 2, 3, CHLR/HTRS-SEQ-2, -1, 720, 0, 0, "The order in which the chiller/heaters are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 2, 3, CHLR/HTRS-MAX-2, -1, 709, 0, 0, "The maximum allowable flow for the chiller/heater"

   SPREAD,  EquipCtrl2DHW, 1565, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		    "DHW Heater Name",  174,  2, 0, 1, 3, 3,     DW-HEATERS-2, -1, 714, 0, 0, "Name of the water heater that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 3, 3, DW-HEATERS-SEQ-2, -1, 720, 0, 0, "The order in which the water heaters are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 3, 3,       MAX-FLOW-2, -1, 709, 0, 0, "The maximum allowable flow for the water heater"

   SPREAD,  EquipCtrl2HR, 1566, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
             "Heat Reject Device",  174,  2, 0, 1, 4, 3,     HEAT-REJ-2, -1, 712, 0, 0, "Name of the heat rejector that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 4, 3, HEAT-REJ-SEQ-2, -1, 720, 0, 0, "The order in which the heat rejectors are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 4, 3,     MAX-FLOW-2, -1, 710, 0, 0, "Maximum allowable flow rate that can be assigned to each heat rejector"

   SPREAD,  EquipCtrl2HR2, 1601, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		         "Ground Loop HX Name",  174,  2, 0, 1, 4, 3,         GLHX-2, -1, 717, 0, 0, "Name of the ground loop heat exchanger that is used to match the corresponding flow range"
		                         "Seq",   35,  0, 0, 1, 4, 3,     GLHX-SEQ-2, -1, 720, 0, 0, "The order in which the ground loop heat exchangers are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 4, 3,     GLHX-MAX-2, -1, 709, 0, 0, "The maximum allowable flow for the ground loop heat exchanger"

   SPREAD,  EquipCtrl2Elec, 1567, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
           "Generator Name",  174,  2, 0, 1, 5, 3,     GENERATORS-2, -1, 714, 0, 0, "Name of the generator that is used to match the corresponding load range"
		                "Seq",   35,  0, 0, 1, 5, 3, GENERATORS-SEQ-2, -1, 720, 0, 0, "The order in which the generators are used to satisfy the load"
		           "Max Load",   75,  2, 0, 1, 5, 3,       MAX-LOAD-2, -1, 709, 0, 0, "The maximum allowable load for the generator"

   ; --- Load Range 3 ---

   SPREAD,  EquipCtrl3Cl, 1568, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		       "Chiller Name",  174,  2, 0, 1, 1, 3,     CHILLERS-3, -1, 719, 0, 0, "Name of the chiller that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 1, 3, CHILLERS-SEQ-3, -1, 720, 0, 0, "The order in which the chillers are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 1, 3,     MAX-FLOW-3, -1, 709, 0, 0, "The maximum allowable flow for the chiller"

   SPREAD,  EquipCtrl3Ht, 1569, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		        "Boiler Name",  174,  2, 0, 1, 2, 3,     BOILERS-3, -1, 721, 0, 0, "Name of the boiler that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 2, 3, BOILERS-SEQ-3, -1, 720, 0, 0, "The order in which the boilers are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 2, 3,    MAX-FLOW-3, -1, 709, 0, 0, "The maximum allowable flow for the boiler"

   SPREAD,  EquipCtrl3Ht2, 1570, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
      "Chiller/Heater Name",  174,  2, 0, 1, 2, 3,     CHLR/HTRS-3, -1, 717, 0, 0, "Name of the chiller/heater that is used to match the corresponding flow"
                      "Seq",   35,  0, 0, 1, 2, 3, CHLR/HTRS-SEQ-3, -1, 720, 0, 0, "The order in which the chiller/heaters are used to satisfy the flow"
                 "Max Flow",   75,  2, 0, 1, 2, 3, CHLR/HTRS-MAX-3, -1, 709, 0, 0, "The maximum allowable flow for the chiller/heater"

   SPREAD,  EquipCtrl3DHW, 1571, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		    "DHW Heater Name",  174,  2, 0, 1, 3, 3,     DW-HEATERS-3, -1, 714, 0, 0, "Name of the water heater that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 3, 3, DW-HEATERS-SEQ-3, -1, 720, 0, 0, "The order in which the water heaters are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 3, 3,       MAX-FLOW-3, -1, 709, 0, 0, "The maximum allowable flow for the water heater"

   SPREAD,  EquipCtrl3HR, 1572, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
       "Heat Reject Device",  174,  2, 0, 1, 4, 3,     HEAT-REJ-3, -1, 712, 0, 0, "Name of the heat rejector that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 4, 3, HEAT-REJ-SEQ-3, -1, 720, 0, 0, "The order in which the heat rejectors are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 4, 3,     MAX-FLOW-3, -1, 710, 0, 0, "Maximum allowable flow rate that can be assigned to each heat rejector"

   SPREAD,  EquipCtrl3HR2, 1602, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		         "Ground Loop HX Name",  174,  2, 0, 1, 4, 3,         GLHX-3, -1, 717, 0, 0, "Name of the ground loop heat exchanger that is used to match the corresponding flow range"
		                         "Seq",   35,  0, 0, 1, 4, 3,     GLHX-SEQ-3, -1, 720, 0, 0, "The order in which the ground loop heat exchangers are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 4, 3,     GLHX-MAX-3, -1, 709, 0, 0, "The maximum allowable flow for the ground loop heat exchanger"

   SPREAD,  EquipCtrl3Elec, 1573, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
           "Generator Name",  174,  2, 0, 1, 5, 3,     GENERATORS-3, -1, 714, 0, 0, "Name of the generator that is used to match the corresponding load range"
		                "Seq",   35,  0, 0, 1, 5, 3, GENERATORS-SEQ-3, -1, 720, 0, 0, "The order in which the generators are used to satisfy the load"
		           "Max Load",   75,  2, 0, 1, 5, 3,       MAX-LOAD-3, -1, 709, 0, 0, "The maximum allowable load for the generator"

   ; --- Load Range 4 ---

   SPREAD,  EquipCtrl4Cl, 1574, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		       "Chiller Name",  174,  2, 0, 1, 1, 3,     CHILLERS-4, -1, 719, 0, 0, "Name of the chiller that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 1, 3, CHILLERS-SEQ-4, -1, 720, 0, 0, "The order in which the chillers are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 1, 3,     MAX-FLOW-4, -1, 709, 0, 0, "The maximum allowable flow for the chiller"

   SPREAD,  EquipCtrl4Ht, 1575, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		        "Boiler Name",  174,  2, 0, 1, 2, 3,     BOILERS-4, -1, 721, 0, 0, "Name of the boiler that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 2, 3, BOILERS-SEQ-4, -1, 720, 0, 0, "The order in which the boilers are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 2, 3,    MAX-FLOW-4, -1, 709, 0, 0, "The maximum allowable flow for the boiler"

   SPREAD,  EquipCtrl4Ht2, 1576, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
      "Chiller/Heater Name",  174,  2, 0, 1, 2, 3,     CHLR/HTRS-4, -1, 717, 0, 0, "Name of the chiller/heater that is used to match the corresponding flow"
                      "Seq",   35,  0, 0, 1, 2, 3, CHLR/HTRS-SEQ-4, -1, 720, 0, 0, "The order in which the chiller/heaters are used to satisfy the flow"
                 "Max Flow",   75,  2, 0, 1, 2, 3, CHLR/HTRS-MAX-4, -1, 709, 0, 0, "The maximum allowable flow for the chiller/heater"

   SPREAD,  EquipCtrl4DHW, 1577, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		    "DHW Heater Name",  174,  2, 0, 1, 3, 3,     DW-HEATERS-4, -1, 714, 0, 0, "Name of the water heater that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 3, 3, DW-HEATERS-SEQ-4, -1, 720, 0, 0, "The order in which the water heaters are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 3, 3,       MAX-FLOW-4, -1, 709, 0, 0, "The maximum allowable flow for the water heater"

   SPREAD,  EquipCtrl4HR, 1578, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
       "Heat Reject Device",  174,  2, 0, 1, 4, 3,     HEAT-REJ-4, -1, 712, 0, 0, "Name of the heat rejector that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 4, 3, HEAT-REJ-SEQ-4, -1, 720, 0, 0, "The order in which the heat rejectors are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 4, 3,     MAX-FLOW-4, -1, 710, 0, 0, "Maximum allowable flow rate that can be assigned to each heat rejector"

   SPREAD,  EquipCtrl4HR2, 1603, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		         "Ground Loop HX Name",  174,  2, 0, 1, 4, 3,         GLHX-4, -1, 717, 0, 0, "Name of the ground loop heat exchanger that is used to match the corresponding flow range"
		                         "Seq",   35,  0, 0, 1, 4, 3,     GLHX-SEQ-4, -1, 720, 0, 0, "The order in which the ground loop heat exchangers are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 4, 3,     GLHX-MAX-4, -1, 709, 0, 0, "The maximum allowable flow for the ground loop heat exchanger"

   SPREAD,  EquipCtrl4Elec, 1579, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
           "Generator Name",  174,  2, 0, 1, 5, 3,     GENERATORS-4, -1, 714, 0, 0, "Name of the generator that is used to match the corresponding load range"
		                "Seq",   35,  0, 0, 1, 5, 3, GENERATORS-SEQ-4, -1, 720, 0, 0, "The order in which the generators are used to satisfy the load"
		           "Max Load",   75,  2, 0, 1, 5, 3,       MAX-LOAD-4, -1, 709, 0, 0, "The maximum allowable load for the generator"

   ; --- Load Range 5 ---

   SPREAD,  EquipCtrl5Cl, 1580, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		       "Chiller Name",  174,  2, 0, 1, 1, 3,     CHILLERS-5, -1, 719, 0, 0, "Name of the chiller that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 1, 3, CHILLERS-SEQ-5, -1, 720, 0, 0, "The order in which the chillers are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 1, 3,     MAX-FLOW-5, -1, 709, 0, 0, "The maximum allowable flow for the chiller"

   SPREAD,  EquipCtrl5Ht, 1581, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		        "Boiler Name",  174,  2, 0, 1, 2, 3,     BOILERS-5, -1, 721, 0, 0, "Name of the boiler that is used to match the corresponding flow"
		                "Seq",   35,  0, 0, 1, 2, 3, BOILERS-SEQ-5, -1, 720, 0, 0, "The order in which the boilers are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 2, 3,    MAX-FLOW-5, -1, 709, 0, 0, "The maximum allowable flow for the boiler"

   SPREAD,  EquipCtrl5Ht2, 1582, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
      "Chiller/Heater Name",  174,  2, 0, 1, 2, 3,     CHLR/HTRS-5, -1, 717, 0, 0, "Name of the chiller/heater that is used to match the corresponding flow range"
                      "Seq",   35,  0, 0, 1, 2, 3, CHLR/HTRS-SEQ-5, -1, 720, 0, 0, "The order in which the chiller/heaters are used to satisfy the flow"
                 "Max Flow",   75,  2, 0, 1, 2, 3, CHLR/HTRS-MAX-5, -1, 709, 0, 0, "The maximum allowable flow for the chiller/heater"

   SPREAD,  EquipCtrl5DHW, 1583, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		    "DHW Heater Name",  174,  2, 0, 1, 3, 3,     DW-HEATERS-5, -1, 714, 0, 0, "Name of the water heater that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 3, 3, DW-HEATERS-SEQ-5, -1, 720, 0, 0, "The order in which the water heaters are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 3, 3,       MAX-FLOW-5, -1, 709, 0, 0, "The maximum allowable flow for the water heater"

   SPREAD,  EquipCtrl5HR, 1584, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
       "Heat Reject Device",  174,  2, 0, 1, 4, 3,     HEAT-REJ-5, -1, 712, 0, 0, "Name of the heat rejector that is used to match the corresponding flow range"
		                "Seq",   35,  0, 0, 1, 4, 3, HEAT-REJ-SEQ-5, -1, 720, 0, 0, "The order in which the heat rejectors are used to satisfy the flow"
		           "Max Flow",   75,  2, 0, 1, 4, 3,     MAX-FLOW-5, -1, 710, 0, 0, "Maximum allowable flow rate that can be assigned to each heat rejector"

   SPREAD,  EquipCtrl5HR2, 1604, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
		         "Ground Loop HX Name",  174,  2, 0, 1, 4, 3,         GLHX-5, -1, 717, 0, 0, "Name of the ground loop heat exchanger that is used to match the corresponding flow range"
		                         "Seq",   35,  0, 0, 1, 4, 3,     GLHX-SEQ-5, -1, 720, 0, 0, "The order in which the ground loop heat exchangers are used to satisfy the flow"
		                    "Max Flow",   75,  2, 0, 1, 4, 3,     GLHX-MAX-5, -1, 709, 0, 0, "The maximum allowable flow for the ground loop heat exchanger"

   SPREAD,  EquipCtrl5Elec, 1585, ACTIVE, NONE, 1, 
			   EQUIP-CTRL, -1, NORMAL, NUMBERS, STD, 30, 20, 0, 3
           "Generator Name",  174,  2, 0, 1, 5, 3,     GENERATORS-5, -1, 714, 0, 0, "Name of the generator that is used to match the corresponding load range"
		                "Seq",   35,  0, 0, 1, 5, 3, GENERATORS-SEQ-5, -1, 720, 0, 0, "The order in which the generators are used to satisfy the load"
		           "Max Load",   75,  2, 0, 1, 5, 3,       MAX-LOAD-5, -1, 709, 0, 0, "The maximum allowable load for the generator"


   ;*****   Load Management Spreadsheets   *****

   ; --- Load Management Seq 1 ---

   SPREAD,  LdMgmt1EquipCtrl1, 1417, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 1, 3,     EQUIP-CTRLS-1, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt1LoopsOn1, 1418, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 1, 3,        LOOPS-ON-1, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt1LoopsOff1, 1419, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 1, 3,        LOOPS-OFF-1, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt1EquipCtrl2, 1420, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 2, 3,     EQUIP-CTRLS-1, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt1LoopsOn2, 1421, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 2, 3,        LOOPS-ON-1, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt1LoopsOff2, 1422, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 2, 3,       LOOPS-OFF-1, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt1EquipCtrl3, 1423, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 3, 3,     EQUIP-CTRLS-1, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt1LoopsOn3, 1424, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 3, 3,        LOOPS-ON-1, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt1LoopsOff3, 1425, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 3, 3,       LOOPS-OFF-1, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt1EquipCtrl4, 1426, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 4, 3,     EQUIP-CTRLS-1, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   ; --- Load Management Seq 2 ---

   SPREAD,  LdMgmt2EquipCtrl1, 1427, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 1, 3,     EQUIP-CTRLS-2, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt2LoopsOn1, 1428, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 1, 3,        LOOPS-ON-2, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt2LoopsOff1, 1429, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 1, 3,       LOOPS-OFF-2, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt2EquipCtrl2, 1430, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 2, 3,     EQUIP-CTRLS-2, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt2LoopsOn2, 1431, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 2, 3,        LOOPS-ON-2, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt2LoopsOff2, 1432, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 2, 3,       LOOPS-OFF-2, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt2EquipCtrl3, 1433, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 3, 3,     EQUIP-CTRLS-2, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt2LoopsOn3, 1434, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 3, 3,        LOOPS-ON-2, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt2LoopsOff3, 1435, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops OFF",  125,  2, 0, 1, 3, 3,       LOOPS-OFF-2, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt2EquipCtrl4, 1436, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 4, 3,     EQUIP-CTRLS-2, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"


   ; --- Load Management Seq 3 ---

   SPREAD,  LdMgmt3EquipCtrl1, 1437, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 1, 3,     EQUIP-CTRLS-3, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt3LoopsOn1, 1438, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 1, 3,        LOOPS-ON-3, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt3LoopsOff1, 1439, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 1, 3,       LOOPS-OFF-3, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt3EquipCtrl2, 1440, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 2, 3,     EQUIP-CTRLS-3, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt3LoopsOn2, 1441, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 2, 3,        LOOPS-ON-3, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt3LoopsOff2, 1442, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 2, 3,       LOOPS-OFF-3, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt3EquipCtrl3, 1443, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 3, 3,     EQUIP-CTRLS-3, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt3LoopsOn3, 1444, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 3, 3,        LOOPS-ON-3, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt3LoopsOff3, 1445, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 3, 3,       LOOPS-OFF-3, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt3EquipCtrl4, 1446, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 4, 3,     EQUIP-CTRLS-3, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   ; --- Load Management Seq 4 ---

   SPREAD,  LdMgmt4EquipCtrl1, 1447, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 1, 3,     EQUIP-CTRLS-4, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt4LoopsOn1, 1448, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 1, 3,        LOOPS-ON-4, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt4LoopsOff1, 1449, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 1, 3,       LOOPS-OFF-4, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt4EquipCtrl2, 1450, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 2, 3,     EQUIP-CTRLS-4, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt4LoopsOn2, 1451, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 2, 3,        LOOPS-ON-4, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt4LoopsOff2, 1452, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 2, 3,       LOOPS-OFF-4, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt4EquipCtrl3, 1453, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 3, 3,     EQUIP-CTRLS-4, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt4LoopsOn3, 1454, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 3, 3,        LOOPS-ON-4, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt4LoopsOff3, 1455, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 3, 3,       LOOPS-OFF-4, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt4EquipCtrl4, 1456, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 4, 3,     EQUIP-CTRLS-4, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   ; --- Load Management Seq 5 ---

   SPREAD,  LdMgmt5EquipCtrl1, 1457, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 1, 3,     EQUIP-CTRLS-5, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt5LoopsOn1, 1458, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 1, 3,        LOOPS-ON-5, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt5LoopsOff1, 1459, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 1, 3,       LOOPS-OFF-5, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt5EquipCtrl2, 1460, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 2, 3,     EQUIP-CTRLS-5, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt5LoopsOn2, 1461, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 2, 3,        LOOPS-ON-5, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt5LoopsOff2, 1462, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 2, 3,       LOOPS-OFF-5, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt5EquipCtrl3, 1463, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 3, 3,     EQUIP-CTRLS-5, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"

   SPREAD,  LdMgmt5LoopsOn3, 1464, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                        "Loops 'ON'",  158,  2, 0, 1, 3, 3,        LOOPS-ON-5, -1, 697, 0, 0, "The loops that are forced to operate this hour"

   SPREAD,  LdMgmt5LoopsOff3, 1465, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		                       "Loops 'OFF'",  158,  2, 0, 1, 3, 3,       LOOPS-OFF-5, -1, 698, 0, 0, "The loops that are forced off this hour"

   SPREAD,  LdMgmt5EquipCtrl4, 1466, ACTIVE, NONE, 1, 
			   LOAD-MANAGEMENT, -1, NORMAL, NUMBERS, STD, 30, 36, 0, 1
		       "Equipment Control Sequences",  158,  2, 0, 1, 4, 3,     EQUIP-CTRLS-5, -1, 699, 0, 0, "Names of Equip Ctrl sequences used when Equip Ctrl Flag or Temp Through condition is true"


   ;*****   Non-Hourly Report Spreadsheets   *****

   SPREAD, NHLoadsSpread, 1706, ACTIVE, NONE, 1, 
   			LOADS-REPORT, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 2
               "Verification Reports",   208,  0, 1, 1, 0, 3, VERIFICATION, -1,     0,     0, 0, ""
               "Summary Reports",        208,  0, 1, 1, 0, 3, SUMMARY,      -1,     0,     0, 0, ""

   SPREAD, NHSysSpread, 1716, ACTIVE, NONE, 1, 
   			SYSTEMS-REPORT, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 2
               "Verification Reports",   208,  0, 1, 1, 0, 3, VERIFICATION, -1,     0,     0, 0, ""
               "Summary Reports",        208,  0, 1, 1, 0, 3, SUMMARY,      -1,     0,     0, 0, ""

   SPREAD, NHPlantSpread, 1726, ACTIVE, NONE, 1, 
   			PLANT-REPORT, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 2
               "Verification Reports",   208,  0, 1, 1, 0, 3, VERIFICATION, -1,     0,     0, 0, ""
               "Summary Reports",        208,  0, 1, 1, 0, 3, SUMMARY,      -1,     0,     0, 0, ""

   SPREAD, NHEconSpread, 1736, ACTIVE, NONE, 1, 
   			ECONOMICS-REPORT, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 2
               "Verification Reports",   208,  0, 1, 1, 0, 3, VERIFICATION, -1,     0,     0, 0, ""
               "Summary Reports",        208,  0, 1, 1, 0, 3, SUMMARY,      -1,     0,     0, 0, ""

   SPREAD, NHDumpLoadsSpread, 1746, ACTIVE, NONE, 1, 
   			LOADS-REPORT, -1, NORMAL, NUMBERS, STD, 20, 20, 0, 1
               "Dump Options",   102,  0, 1, 1, 0, 3, DUMP-OPTIONS, -1,     0,     0, 0, ""

   SPREAD, NHDumpSysSpread, 1756, ACTIVE, NONE, 1, 
   			SYSTEMS-REPORT, -1, NORMAL, NUMBERS, STD, 20, 20, 0, 1
               "Dump Options",   102,  0, 1, 1, 0, 3, DUMP-OPTIONS, -1,     0,     0, 0, ""

   SPREAD, NHDumpPlantSpread, 1766, ACTIVE, NONE, 1, 
   			PLANT-REPORT, -1, NORMAL, NUMBERS, STD, 20, 20, 0, 1
               "Dump Options",   102,  0, 1, 1, 0, 3, DUMP-OPTIONS, -1,     0,     0, 0, ""

   SPREAD, NHDumpEconSpread, 1776, ACTIVE, NONE, 1, 
   			ECONOMICS-REPORT, -1, NORMAL, NUMBERS, STD, 20, 20, 0, 1
               "Dump Options",   102,  0, 1, 1, 0, 3, DUMP-OPTIONS, -1,     0,     0, 0, ""


   ;*****   Baseline Costs Spreadsheet   *****

   SPREAD,  Baseline, 1517, ACTIVE, NONE, 1, 
			   BASELINE, -1, NORMAL, YEAR, STD, 60, 36, 0, 2
               "Utility Annual Costs",     100,  2, 1, 1, 0, 3,      ENERGY-COST, -1, 750, 0, 0, "Present Value of the baseline energy cost for each year of the project"
		         "Operations Annual Costs",  123,  2, 1, 1, 0, 3,  OPERATIONS-COST, -1, 749, 0, 0, "Present Value of the baseline operations costs for each year of the project"


   ;*****   Compliance DHW Spreadsheet   *****

   SPREAD, CompDHWLoopsSpread, 9400, ACTIVE, NONE, 1, 
   			COMPLIANCE-DHW, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 1
               "HW/DHW Circulation Loops",   200, 32, 1, 1,  1, 1, C-LOOPS,     -1,      0,     0,  0, "The name of the attached HW or DHW circulation loop"


   ;*****   Elec Meter - UTILITY (TYPE = 1) - Interior Direct Loads Spreadsheet   *****
   SPREAD, EMtr1IntLoadsSpread, 1800, ACTIVE, NONE, 1, 
            ELEC-METER, 1, NORMAL, NUMBERS, STD, 25, 20, 0, 3
				   "Load",        90,  2, 1, 1, 0, 3, INTERIOR-POWER,      -1,   736, 32075, 0, "Hourly internal energy consumption (typically use Loop Process Loads instead)"
				   "Schedule",   200,  0, 1, 1, 0, 3, INTERIOR-SCH,        -1,   735, 32075, 0, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
				   "Enduse",     140,  1, 1, 1, 0, 3, INTERIOR-EU,         -1,     0, 32075, 0, "Enduse to apply this energy use to"

   ;*****   Elec Meter - BUILDING (TYPE = 2) - Interior Direct Loads Spreadsheet   *****
   SPREAD, EMtr2IntLoadsSpread, 1801, ACTIVE, NONE, 1, 
            ELEC-METER, 2, NORMAL, NUMBERS, STD, 25, 20, 0, 3
				   "Load",        90,  2, 1, 1, 0, 3, INTERIOR-POWER,      -1,   736, 32075, 0, "Hourly internal energy consumption (typically use Loop Process Loads instead)"
				   "Schedule",   200,  0, 1, 1, 0, 3, INTERIOR-SCH,        -1,   735, 32075, 0, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
				   "Enduse",     140,  1, 1, 1, 0, 3, INTERIOR-EU,         -1,     0, 32075, 0, "Enduse to apply this energy use to"

   ;*****   Elec Meter - SUB-METER (TYPE = 3) - Interior Direct Loads Spreadsheet   *****
   SPREAD, EMtr3IntLoadsSpread, 1802, ACTIVE, NONE, 1, 
            ELEC-METER, 3, NORMAL, NUMBERS, STD, 25, 20, 0, 3
				   "Load",        90,  2, 1, 1, 0, 3, INTERIOR-POWER,      -1,   736, 32075, 0, "Hourly internal energy consumption (typically use Loop Process Loads instead)"
				   "Schedule",   200,  0, 1, 1, 0, 3, INTERIOR-SCH,        -1,   735, 32075, 0, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
				   "Enduse",     140,  1, 1, 1, 0, 3, INTERIOR-EU,         -1,     0, 32075, 0, "Enduse to apply this energy use to"

; SAC 9/21/04 - Added access to new EXTERIOR-EU keyword
   ;*****   Elec Meter - UTILITY (TYPE = 1) - Exterior Direct Loads Spreadsheet   *****
   SPREAD, EMtr1ExtLoadsSpread, 1810, ACTIVE, NONE, 1, 
            ELEC-METER, 1, NORMAL, NUMBERS, STD, 25, 20, 0, 3
				   "Load",        90,  2, 1, 1, 0, 3, EXTERIOR-POWER,      -1,   736, 32075, 0, "Hourly internal energy consumption (typically use Loop Process Loads instead)"
				   "Schedule",   200,  0, 1, 1, 0, 3, EXTERIOR-SCH,        -1,   735, 32075, 0, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
				   "Enduse",     140,  1, 1, 1, 0, 3, EXTERIOR-EU,         -1,     0, 32075, 0, "Enduse to apply this energy use to"

   ;*****   Elec Meter - BUILDING (TYPE = 2) - Exterior Direct Loads Spreadsheet   *****
   SPREAD, EMtr2ExtLoadsSpread, 1811, ACTIVE, NONE, 1, 
            ELEC-METER, 2, NORMAL, NUMBERS, STD, 25, 20, 0, 3
				   "Load",        90,  2, 1, 1, 0, 3, EXTERIOR-POWER,      -1,   736, 32075, 0, "Hourly internal energy consumption (typically use Loop Process Loads instead)"
				   "Schedule",   200,  0, 1, 1, 0, 3, EXTERIOR-SCH,        -1,   735, 32075, 0, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
				   "Enduse",     140,  1, 1, 1, 0, 3, EXTERIOR-EU,         -1,     0, 32075, 0, "Enduse to apply this energy use to"

   ;*****   Elec Meter - SUB-METER (TYPE = 3) - Exterior Direct Loads Spreadsheet   *****
   SPREAD, EMtr3ExtLoadsSpread, 1812, ACTIVE, NONE, 1, 
            ELEC-METER, 3, NORMAL, NUMBERS, STD, 25, 20, 0, 3
				   "Load",        90,  2, 1, 1, 0, 3, EXTERIOR-POWER,      -1,   736, 32075, 0, "Hourly internal energy consumption (typically use Loop Process Loads instead)"
				   "Schedule",   200,  0, 1, 1, 0, 3, EXTERIOR-SCH,        -1,   735, 32075, 0, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
				   "Enduse",     140,  1, 1, 1, 0, 3, EXTERIOR-EU,         -1,     0, 32075, 0, "Enduse to apply this energy use to"


   ;*****   Fuel Meter - Interior Direct Loads Spreadsheet   *****
   SPREAD, FMtrIntLoadsSpread, 1820, ACTIVE, NONE, 1, 
            FUEL-METER, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 3
				   "Load",       110,  2, 1, 1, 0, 3, INTERIOR-POWER,      -1,   736, 32075, 0, "Hourly internal energy consumption (typically use Loop Process Loads instead)"
				   "Schedule",   200,  0, 1, 1, 0, 3, INTERIOR-SCH,        -1,   735, 32075, 0, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
				   "Enduse",     140,  1, 1, 1, 0, 3, INTERIOR-EU,         -1,     0, 32075, 0, "Enduse to apply this energy use to"

; SAC 9/27/04 - Added access to new EXTERIOR-EU keyword
   ;*****   Fuel Meter - Exterior Direct Loads Spreadsheet   *****
   SPREAD, FMtrExtLoadsSpread, 1821, ACTIVE, NONE, 1, 
            FUEL-METER, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 3
				   "Load",       110,  2, 1, 1, 0, 3, EXTERIOR-POWER,      -1,   736, 32075, 0, "Hourly internal energy consumption (typically use Loop Process Loads instead)"
				   "Schedule",   200,  0, 1, 1, 0, 3, EXTERIOR-SCH,        -1,   735, 32075, 0, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
				   "Enduse",     140,  1, 1, 1, 0, 3, EXTERIOR-EU,         -1,     0, 32075, 0, "Enduse to apply this energy use to"


   ;*****   Master Meters - Exclude From TDV Spreadsheet   *****  - SAC 9/21/04
   SPREAD, MstMtrExclTDVSpread, 1822, ACTIVE, NONE, 1, 
            MASTER-METERS, -1, NORMAL, NUMBERS, STD, 25, 20, 0, 1
				   "Exclude Enduse(s)",  180,  1, 1, 1, 0, 3, EXCLUDE-FROM-TDV,   -1,     0, 32075, 0, "Enduse to exclude from the time dependent valuation (TDV) calculations"
				   
 ;*****   Added access to new PROJECT-DATA command   *****  - TWV 8/12/12
   SPREAD, ProjectDataSpread, 1823, ACTIVE, NONE, 1, 
            PROJECT-DATA, -1, TRANSPOSE, NONE, STD, 180, 20, 0, 38
				   "Area Per Floor",  180,  1, 1, 1, 0, 3, AREA-PER-FLR,   -1,     0, 32075, 0, "Area Per Floor"
				   "Floor Length",    180,  1, 1, 1, 0, 3, FLOOR-LENGTH,   -1,     0, 32075, 0, "Floor Length"
					 "Floor Width",     180,  1, 1, 1, 0, 3, FLOOR-WIDTH,    -1,     0, 32075, 0, "Floor Width"	
           "One Level Area",  180,  1, 1, 1, 0, 3, ONE-LEVEL-AREA, -1,     0, 32075, 0, "One Level Area"	
           "Two Level Area",  180,  1, 1, 1, 0, 3, TWO-LEVEL-AREA, -1,     0, 32075, 0, "Two Level Area"	
           "Attic Area",      180,  1, 1, 1, 0, 3, ATTIC-AREA,     -1,     0, 32075, 0, "Attic Area"	
           "Attic Height",    180,  1, 1, 1, 0, 3, ATTIC-HEIGHT,   -1,     0, 32075, 0, "Attic Height"	
           "Cathedral Length",180,  1, 1, 1, 0, 3, CATHEDRAL-LENGTH,-1,    0, 32075, 0, "Cathedral Length"	
           "Cathedral Width", 180,  1, 1, 1, 0, 3, CATHEDRAL-WIDTH,-1,     0, 32075, 0, "Cathedral Width"	
           "Typ. Window Width",180, 1, 1, 1, 0, 3, TYP-WIN-WIDTH,  -1,     0, 32075, 0, "Typical Window Width"	
           "Typ. Window Height",180,1, 1, 1, 0, 3, TYP-WIN-Y,      -1,     0, 32075, 0, "Typical Window Height"	
           "Window Spacing 1",180,  1, 1, 1, 0, 3, WIN-SPACING1,   -1,     0, 32075, 0, "Window Spacing 1"	
           "Window Spacing 2",180,  1, 1, 1, 0, 3, WIN-SPACING2,   -1,     0, 32075, 0, "Window Spacing 2"
           "2 Level Slab R",  180,  1, 1, 1, 0, 3, TWO-LEVEL-SLAB-R,-1,    0, 32075, 0, "2 Level Slab R-Value"	
           "1 Level Slab R",  180,  1, 1, 1, 0, 3, ONE-LEVEL-SLAB-R,-1,    0, 32075, 0, "1 Level Slab R-Value"	
           "Crawlspace Eff R",180,  1, 1, 1, 0, 3, CRAWL-R-EFF,    -1,     0, 32075, 0, "Crawl space effective R-Value"	
           "Shad Short",      180,  1, 1, 1, 0, 3, SHAD-SHORT,     -1,     0, 32075, 0, "Shad Short"	
           "Shad Long",       180,  1, 1, 1, 0, 3, SHAD-LONG,      -1,     0, 32075, 0, "Shad Long"	
           "Variable01",      180,  1, 1, 1, 0, 3, Variable01,     -1,     0, 32075, 0, "Variable01"	
           "Variable02",      180,  1, 1, 1, 0, 3, Variable02,     -1,     0, 32075, 0, "Variable02"	
           "Variable03",      180,  1, 1, 1, 0, 3, Variable03,     -1,     0, 32075, 0, "Variable03"	
           "Variable04",      180,  1, 1, 1, 0, 3, Variable04,     -1,     0, 32075, 0, "Variable04"	
           "Variable05",      180,  1, 1, 1, 0, 3, Variable05,     -1,     0, 32075, 0, "Variable05"
           "Variable06",      180,  1, 1, 1, 0, 3, Variable06,     -1,     0, 32075, 0, "Variable06"	
           "Variable07",      180,  1, 1, 1, 0, 3, Variable07,     -1,     0, 32075, 0, "Variable07"
           "Variable08",      180,  1, 1, 1, 0, 3, Variable08,     -1,     0, 32075, 0, "Variable08"
           "Variable09",      180,  1, 1, 1, 0, 3, Variable09,     -1,     0, 32075, 0, "Variable09"
           "Variable10",      180,  1, 1, 1, 0, 3, Variable10,     -1,     0, 32075, 0, "Variable10"
           "Variable11",      180,  1, 1, 1, 0, 3, Variable11,     -1,     0, 32075, 0, "Variable11"
           "Variable12",      180,  1, 1, 1, 0, 3, Variable12,     -1,     0, 32075, 0, "Variable12"
           "Variable13",      180,  1, 1, 1, 0, 3, Variable13,     -1,     0, 32075, 0, "Variable13"
           "Variable14",      180,  1, 1, 1, 0, 3, Variable14,     -1,     0, 32075, 0, "Variable14"
           "Variable15",      180,  1, 1, 1, 0, 3, Variable15,     -1,     0, 32075, 0, "Variable15"
           "Variable16",      180,  1, 1, 1, 0, 3, Variable16,     -1,     0, 32075, 0, "Variable16"
           "Variable17",      180,  1, 1, 1, 0, 3, Variable17,     -1,     0, 32075, 0, "Variable17"
           "Variable18",      180,  1, 1, 1, 0, 3, Variable18,     -1,     0, 32075, 0, "Variable18"
           "Variable19",      180,  1, 1, 1, 0, 3, Variable19,     -1,     0, 32075, 0, "Variable19"
           "Variable20",      180,  1, 1, 1, 0, 3, Variable20,     -1,     0, 32075, 0, "Variable20"	
					 									 
					 ; TV-These values Made Row headers narrow            PROJECT-DATA, -1, TRANSPOSE, NUMBERS, STD, 15, 20, 0, 2	   


; SAC 2/28/07 - REMOVED MAINSPREAD definitions - replaced w/ data stored in BDLUIData.csv
;  ; 
;  ; Punt For Now:
;  ; 
;  ; HEAT-EXCHANGER      -4  - ??? (exclude for now)
;  ; EQUIP-CTRL          -5  - Don't imp for now
;  ; LOAD-MANAGEMENT     -4  - Don't imp for now
;  ; GROUND-LOOP-HX      -4  - ??? (exclude for now)
;  ; 
;  
;  ; ************** START OF MAINSPREAD *************************
;  
;  MAINSPREAD, PARAMETER, -1, "Parameters",                                                    1
;  MAINSPREAD, SITE-PARAMETERS, -1, "Site Parameters",                                         2
;  MAINSPREAD, DESIGN-DAY, -1, "Design Day",                                                   3
;  MAINSPREAD, BUILD-PARAMETERS, -1, "Build Parameters",                                       4
;  MAINSPREAD, BUILDING-SHADE, -1, "Building Shade",                                           5
;  MAINSPREAD, FIXED-SHADE, -1, "Fixed Shade",                                                 6
;  MAINSPREAD, FLOOR, -1, "Floor",                                                             7
;  ; i1 Index of 8 here for start of spaces
;  MAINSPREAD, SPACE, -1, "General",                                                           8
;  MAINSPREAD, SPACE, -1, "Occupancy",                                                         9
;  MAINSPREAD, SPACE, -1, "Lighting",                                                         10
;  MAINSPREAD, SPACE, -1, "Daylighting",                                                      11
;  MAINSPREAD, SPACE, -1, "Equipment",                                                        12
;  MAINSPREAD, SPACE, -1, "Internal Energy Sources",                                          13
;  MAINSPREAD, SPACE, -1, "Infiltration",                                                     14
;  MAINSPREAD, SPACE, -1, "Internal Mass",                                                    15
;  MAINSPREAD, EXTERIOR-WALL, -1, "Exterior Walls",                                           16
;  MAINSPREAD, INTERIOR-WALL, -1, "Interior Walls",                                           17
;  MAINSPREAD, UNDERGROUND-WALL, -1, "Underground Walls",                                     18
;  MAINSPREAD, WINDOW, -1, "Basic Specifications",                                            19
;  MAINSPREAD, WINDOW, -1, "Fins & Overhang",                                                 20    ; SAC 7/28/03 - Split WINDOW into Basic vs. "Fins & Overhang"
;  MAINSPREAD, GLASS-TYPE, -1, "Glass Type",                                                  21
;  MAINSPREAD, DOOR, -1, "Doors",                                                             22
;  MAINSPREAD, CONSTRUCTION, -1, "Constructions",                                             23
;  MAINSPREAD, LAYERS, -1, "Layers",                                                          24
;  MAINSPREAD, MATERIAL, -1, "Materials",                                                     25
;  MAINSPREAD, ZONE, -1, "Basic Specifications",                                              26
;  MAINSPREAD, ZONE, -1, "Air Flow",                                                          27
;  MAINSPREAD, ZONE, -1, "Outside Air & Exhaust",                                             28
;  MAINSPREAD, ZONE, -1, "Cooling",                                                           29
;  MAINSPREAD, ZONE, -1, "Heating",                                                           30
;  MAINSPREAD, ZONE, -1, "Meters",                                                            31
;  MAINSPREAD, ZONE, -1, "Sun Space",                                                         32
;  MAINSPREAD, ZONE, -1, "Refigeration",                                                      33
;  MAINSPREAD, SYSTEM, -1, "Basic Specifications",                                            34
;  MAINSPREAD, SYSTEM, -1, "Humidity Control",                                                35
;  MAINSPREAD, SYSTEM, -1, "Duct Losses",                                                     36
;  MAINSPREAD, SYSTEM, -1, "Staged Volume",                                                   37
;  MAINSPREAD, SYSTEM, -1, "Fans - Fan Control",                                              38
;  MAINSPREAD, SYSTEM, -1, "Fans - Fan Power",                                                39
;  MAINSPREAD, SYSTEM, -1, "Fans - Flow Parameters",                                          40
;  MAINSPREAD, SYSTEM, -1, "Fans - Night Cycle Control",                                      41
;  MAINSPREAD, SYSTEM, -1, "Outdoor Air - Vent & Economizer",                                 42
;  ; MAINSPREAD, SYSTEM, -1, "Outdoor Air - Heat Recovery",                                   42      ; SAC 1/16/02 - Removed
;  MAINSPREAD, SYSTEM, -1, "Outdoor Air - Natural Ventilation",                               43
;  MAINSPREAD, SYSTEM, -1, "Cooling - Coil Capacity",                                         44
;  MAINSPREAD, SYSTEM, -1, "Cooling - Control",                                               45
;  MAINSPREAD, SYSTEM, -1, "Cooling - Unitary Power",                                         46
;  MAINSPREAD, SYSTEM, -1, "Cooling - Condenser",                                             47
;  MAINSPREAD, SYSTEM, -1, "Cooling - Capacity Curves",                                       48
;  MAINSPREAD, SYSTEM, -1, "Cooling - Evaporative Cooling",                                   49
;  MAINSPREAD, SYSTEM, -1, "Cooling - Water-source Economizer",                               50
;  MAINSPREAD, SYSTEM, -1, "Heating - Coil Capacity",                                         51
;  MAINSPREAD, SYSTEM, -1, "Heating - Control",                                               52
;  MAINSPREAD, SYSTEM, -1, "Heating - Unitary Power",                                         53
;  MAINSPREAD, SYSTEM, -1, "Heating - Preheat",                                               54
;  MAINSPREAD, SYSTEM, -1, "Heating - Baseboard",                                             55
;  MAINSPREAD, SYSTEM, -1, "Heating - Supplemental",                                          56
;  MAINSPREAD, SYSTEM, -1, "Heating - Capacity Curves",                                       57
;  MAINSPREAD, SYSTEM, -1, "Energy Recovery Ventilators - Type and Flow",                     58      ; SAC 1/16/02 - Added
;  MAINSPREAD, SYSTEM, -1, "Energy Recovery Ventilators - Heat Transfer Performance",         59      ; SAC 1/16/02 - Added
;  MAINSPREAD, SYSTEM, -1, "Energy Recovery Ventilators - Control Sequences",                 60      ; SAC 1/16/02 - Added
;  MAINSPREAD, SYSTEM, -1, "Energy Recovery Ventilators - Power Consumption",                 61      ; SAC 1/16/02 - Added
;  MAINSPREAD, SYSTEM, -1, "Energy Recovery Ventilators - Condens/Frost Counteraction",       62      ; SAC 1/16/02 - Added
;  MAINSPREAD, SYSTEM, -1, "Preconditioner - Add-On Evap Cooling",                            63
;  MAINSPREAD, SYSTEM, -1, "Preconditioner - Add-On Desiccant",                               64
;  MAINSPREAD, SYSTEM, -1, "Preconditioner - Package Desiccant",                              65
;  MAINSPREAD, SYSTEM, -1, "Preconditioner - Desiccant Performance Curves",                   66
;  MAINSPREAD, SYSTEM, -1, "System Meters",                                                   67
;  MAINSPREAD, SYSTEM, -1, "Refrigeration - Design Parameters",                               68
;  MAINSPREAD, SYSTEM, -1, "Refrigeration - Condenser",                                       69
;  MAINSPREAD, SYSTEM, -1, "Refrigeration - Heat Recovery",                                   70
;  MAINSPREAD, SYSTEM, -1, "Refrigeration - Anti-Sweat",                                      71
;  MAINSPREAD, SYSTEM, -1, "Refrigeration - Performance Curves",                              72
;  MAINSPREAD, CIRCULATION-LOOP, -1, "Parameters",                                            73
;  MAINSPREAD, CIRCULATION-LOOP, -1, "Losses",                                                74
;  MAINSPREAD, CIRCULATION-LOOP, -1, "Head",                                                  75
;  MAINSPREAD, CIRCULATION-LOOP, -1, "Operation",                                             76
;  MAINSPREAD, CIRCULATION-LOOP, -1, "Controls",                                              77
;  MAINSPREAD, CIRCULATION-LOOP, -1, "Auxiliaries",                                           78
;  MAINSPREAD, CIRCULATION-LOOP, -1, "Process",                                               79
;  MAINSPREAD, PUMP, -1, "Pumps",                                                             80
;  MAINSPREAD, CHILLER, -1, "Basic Specifications",                                           81
;  MAINSPREAD, CHILLER, -1, "Performance Curves",                                             82
;  MAINSPREAD, CHILLER, -1, "Attachments",                                                    83
;  MAINSPREAD, CHILLER, -1, "Miscellaneous",                                                  84
;  MAINSPREAD, BOILER, -1, "Basic Specifications",                                            85
;  MAINSPREAD, BOILER, -1, "Performance Curves",                                              86
;  MAINSPREAD, BOILER, -1, "Attachments",                                                     87
;  MAINSPREAD, BOILER, -1, "Miscellaneous",                                                   88
;  MAINSPREAD, DW-HEATER, -1, "Basic Specifications",                                         89
;  MAINSPREAD, DW-HEATER, -1, "Performance Curves",                                           90
;  MAINSPREAD, DW-HEATER, -1, "Attachments",                                                  91
;  MAINSPREAD, DW-HEATER, -1, "Miscellaneous",                                                92
;  MAINSPREAD, HEAT-REJECTION, -1, "Basic Specifications",                                    93
;  MAINSPREAD, HEAT-REJECTION, -1, "Fluid and Dry Coolers",                                   94
;  MAINSPREAD, HEAT-REJECTION, -1, "Performance Curves",                                      95
;  MAINSPREAD, HEAT-REJECTION, -1, "Attachments",                                             96
;  MAINSPREAD, HEAT-REJECTION, -1, "Miscellaneous",                                           97
;  MAINSPREAD, THERMAL-STORAGE, 1, "Basic Specifications",                                    98
;  MAINSPREAD, THERMAL-STORAGE, 1, "Performance Curves",                                      99
;  MAINSPREAD, THERMAL-STORAGE, 1, "Miscellaneous",                                          100
;  MAINSPREAD, THERMAL-STORAGE, 2, "Basic Specifications",                                   101
;  MAINSPREAD, THERMAL-STORAGE, 2, "Performance Curves",                                     102
;  MAINSPREAD, THERMAL-STORAGE, 2, "Miscellaneous",                                          103
;  MAINSPREAD, ELEC-METER, -1, "Basic Specifications",                                       104
;  MAINSPREAD, ELEC-METER, -1, "Direct Loads - Interior",                                    105
;  MAINSPREAD, ELEC-METER, -1, "Direct Loads - Exterior",                                    106
;  MAINSPREAD, FUEL-METER, -1, "Basic Specifications",                                       107
;  MAINSPREAD, FUEL-METER, -1, "Direct Loads - Interior",                                    108
;  MAINSPREAD, FUEL-METER, -1, "Direct Loads - Exterior",                                    109
;  MAINSPREAD, STEAM-METER, -1, "Basic Specifications",                                      110
;  MAINSPREAD, STEAM-METER, -1, "Direct Loads - Interior",                                   111      ; SAC 9/27/04 - Split out Int/Ext Direct Loads into separate modes
;  MAINSPREAD, STEAM-METER, -1, "Direct Loads - Exterior",                                   112      ; SAC 9/27/04 - Split out Int/Ext Direct Loads into separate modes
;  MAINSPREAD, CHW-METER, -1, "Basic Specifications",                                        113
;  MAINSPREAD, CHW-METER, -1, "Direct Loads - Interior",                                     114      ; SAC 9/27/04 - Split out Int/Ext Direct Loads into separate modes
;  MAINSPREAD, CHW-METER, -1, "Direct Loads - Exterior",                                     115      ; SAC 9/27/04 - Split out Int/Ext Direct Loads into separate modes
;  MAINSPREAD, MATERIALS-COST, -1, "Materials Costs",                                        116
;  MAINSPREAD, COMPONENT-COST, -1, "Component Costs",                                        117
;  MAINSPREAD, BASELINE, -1, "Baseline",                                                     118
;  MAINSPREAD, CURVE-FIT, -1, "Curve Fits",                                                  119
;  MAINSPREAD, GLASS-TYPE-CODE, -1, "General",                                               120
;  MAINSPREAD, GLASS-TYPE-CODE, -1, "Glass Layers",                                          121
;  MAINSPREAD, GLASS-TYPE-CODE, -1, "Gaps Between Layers",                                   122
;  MAINSPREAD, GLASS-TYPE-CODE, -1, "Solar/Optical Details",                                 123
;  MAINSPREAD, WALL-PARAMETERS, -1, "Wall Parameters",                                       124
;  
;  ; ************* END OF MAINSPREAD **********************



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Global Parameters Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

 MODTABDLG, 3201, 0, 1, 30, 30, 330, 520, 0, PARAMETER, "Global Parameters", NOTIMP, 0, NOTIMP, 0

     SPREAD, 11694, 11694, 0, 1, 0, PowerDOE, 0, ParamSpread,  0, STD, 25, 25, 300, 480, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, "global parameters"

    
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Design Day - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; MODDLG, 2519, 2519, 1, 40, 90, 280, 570, 0, "Design Day Data", NOTIMP, 0, NOTIMP, 0 
 MODTABDLG, 2519, 2519, 1, 30, 30, 360, 520, 0, DESIGN-DAY, "Design Day Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 19190,   687, 0, 1, DESIGN-DAY, 0, NAME,  0, STD, 195,  15, 400, 180, 19, 3, "Currently Active Design Day:",  LEFT, -175, 5, 0, LEFT, 4, 5, "List of all design days defined in project; also allows library retrieval and creation"
   STATIC, 1, DESIGN-DAY, 0, TYPE, 0, 0, 0, 400, 20, 150, STD, LEFT, "Type:  ",   "", 0, 3

    ;******************************************
    ; Design Day - Basic Specs Page
    ;******************************************
    TABPAGE, 3197, 2519, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 14813,   687, 0, 1, DESIGN-DAY, 0,            NAME, -1, STD, 130,  10,  23, 200, 32, 3,     "Design Day Name:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Name of design day; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 14814,  1514, 0, 1, DESIGN-DAY, 0,            TYPE,  0, STD, 130,  40, 300,  85, 19, 3,                "Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, ""

       EDIT, 14815, 12737, 0, 1, DESIGN-DAY, 0,    DRYBULB-HIGH, -1, STD, 130,  70,  23,  60,  1, 3,        "Drybulb High:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
       EDIT, 14816, 12738, 0, 1, DESIGN-DAY, 0,   DRYBULB-RANGE, -1, STD, 130,  95,  23,  60,  1, 3,       "Drybulb Range:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
       EDIT, 14817,  1516, 0, 1, DESIGN-DAY, 0, WETBULB-AT-HIGH, -1, STD, 130, 120,  23,  60,  1, 3,     "Wetbulb at High:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""

       EDIT, 14818, 12739, 0, 1, DESIGN-DAY, 0,       HOUR-HIGH, -1, STD, 130, 145,  23,  60,  0, 3,           "Hour High:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
       EDIT, 14819, 12740, 0, 1, DESIGN-DAY, 0,        HOUR-LOW, -1, STD, 130, 170,  23,  60,  0, 3,            "Hour Low:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
       EDIT, 14820,  1513, 0, 1, DESIGN-DAY, 0,           MONTH, -1, STD, 130, 195,  23,  60,  0, 3,        "Month Number:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
       EDIT, 14821,  1512, 0, 1, DESIGN-DAY, 0,             DAY, -1, STD, 130, 220,  23,  60,  0, 3,           "Start Day:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
       EDIT, 14856,  1512, 0, 1, DESIGN-DAY, 0,  NUMBER-OF-DAYS, -1, STD, 130, 245,  23,  60,  0, 3,      "Number of days:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""

       EDIT, 14822, 12747, 0, 1, DESIGN-DAY, 0,    CLOUD-AMOUNT, -1, STD, 410,  70,  23,  50,  0, 3,        "Cloud Amount:",  LEFT, -140, 5, 1, LEFT, 4, 5, ""
       EDIT, 14823,   812, 0, 1, DESIGN-DAY, 0,        GROUND-T, -1, STD, 410,  95,  23,  50,  1, 3,  "Ground Temperature:",  LEFT, -140, 5, 1, LEFT, 4, 5, ""
       EDIT, 14824, 12745, 0, 1, DESIGN-DAY, 0,      WIND-SPEED, -1, STD, 410, 120,  23,  50,  1, 3,          "Wind Speed:",  LEFT, -140, 5, 1, LEFT, 4, 5, ""
      COMBO, 14825, 12746, 0, 1, DESIGN-DAY, 0,        WIND-DIR,  0, STD, 370, 145, 300, 125, 19, 3,      "Wind Direction:",  LEFT, -100, 5, 0, LEFT, 4, 5, ""
      COMBO, 14826,  1511, 0, 1, DESIGN-DAY, 0,         CLIMATE,  0, STD, 370, 170, 120, 125, 19, 3,             "Climate:",  LEFT, -100, 5, 0, LEFT, 4, 5, ""
      COMBO, 14827,  1515, 0, 1, DESIGN-DAY, 0,      VISIBILITY,  0, STD, 370, 195, 120, 125, 19, 3,          "Visibility:",  LEFT, -100, 5, 0, LEFT, 4, 5, ""


 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Run Period - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; MODDLG, 2600, 2600, 1, 200, 200, 165, 345, 0, "Edit Run Period", NOTIMP, 0, NOTIMP, 0
 MODTABDLG, 2600, 2600, 1, 30, 30, 220, 365, 0, RUN-PERIOD, "Run Period Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 14863, 14863, 0, 1, RUN-PERIOD, 0, NAME,  0, STD, 195,  15, 400, 150, 19, 3, "Currently Active Run Period:",  LEFT, -175, 5, 0, LEFT, 4, 5, "List of all run periods defined in project; also allows library retrieval and creation"

    ;******************************************
    ; Design Day - Basic Specs Page
    ;******************************************
    TABPAGE, 3198, 2600, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 14864, 14864, 0, 1, RUN-PERIOD, 0,        NAME, -1, STD, 130,  10,  23, 200, 32, 3,  "Run Period Name:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Name of run period; right mouse quick menu options allow deleting, copying, linking and saving to library"
 
      LABEL, "Month", STD, CENTER, 150, 47, 1, 0, 0, 0, 0, 3
      LABEL,   "Day", STD, CENTER, 205, 47, 1, 0, 0, 0, 0, 3
      LABEL,  "Year", STD, CENTER, 265, 47, 1, 0, 0, 0, 0, 3
    
       EDIT, 13007, 13007, 0, 1, RUN-PERIOD, 0, BEGIN-MONTH,  0, STD, 130,  65,  23,  40,  0, 3,  "Starting:",  LEFT, -60, 5, 0, LEFT, 4, 5, "Beginning month of the simulation"
       EDIT, 13009, 13009, 0, 1, RUN-PERIOD, 0,   BEGIN-DAY,  0, STD, 185,  65,  23,  40,  0, 3,           "",  LEFT,  -2, 5, 0, LEFT, 4, 5, "Beginning day of the simulation"
       EDIT, 13011, 13011, 0, 1, RUN-PERIOD, 0,  BEGIN-YEAR,  0, STD, 240,  65,  23,  50,  0, 3,           "",  LEFT,  -2, 5, 0, LEFT, 4, 5, "Beginning year of the simulation"
       EDIT, 13008, 13008, 0, 1, RUN-PERIOD, 0,   END-MONTH,  0, STD, 130,  95,  23,  40,  0, 3,    "Ending:",  LEFT, -60, 5, 0, LEFT, 4, 5, "Last month of the simulation"
       EDIT, 13010, 13010, 0, 1, RUN-PERIOD, 0,     END-DAY,  0, STD, 185,  95,  23,  40,  0, 3,           "",  LEFT,  -2, 5, 0, LEFT, 4, 5, "Last day of the simulation"
       EDIT, 13012, 13012, 0, 1, RUN-PERIOD, 0,    END-YEAR,  0, STD, 240,  95,  23,  50,  0, 3,           "",  LEFT,  -2, 5, 0, LEFT, 4, 5, "Last year of the simulation"


 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Holidays - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
                          
; MODDLG, 2501, 12543, 1, 160, 160, 355, 305, 0, "Holidays Data", NOTIMP, 0, NOTIMP, 0 
 MODTABDLG, 2501, 12543, 1, 160, 160, 410, 405, 0, HOLIDAYS, "Holiday Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 19160, 12543, 12543, 1,  HOLIDAYS,     0,    NAME,  0, STD, 185,  15, 400, 200, 19, 3, "Currently Active Holidays:", LEFT, -165, 5, 0, LEFT, 4, 5, "This list contains all Holiday sets defined in the project"

    ;******************************************
    ; Holidays - Basic Specs Page
    ;******************************************
    TABPAGE, 3215, 12543, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 19161, 19161, 12543, 1,  HOLIDAYS, 0,    NAME, -1, STD, 125,  10,  23, 226, 32, 3,  "Holidays Name:",  LEFT, -105, 5, 0, LEFT, 4, 5, "Name of holiday set; right mouse quick menu options allow deleting, copying, linking and saving to library"

      COMBO, 14534, 14534, 12543, 1,  HOLIDAYS, 0,    TYPE, -1, STD, 125,  40, 300, 140, 19, 3,  "Holidays Type:",  LEFT, -105, 5, 0, LEFT, 4, 5, "Whether the official US Holidays are used, or none, or a custom set of Holidays"

      CASE,  HOLIDAYS,  0, TYPE,  -1, =, 1, 3
        SPREAD, 11668, 11668,  0, 1, 0, PowerDOE,  0, HolidaySpread,  0, STD, 125,  80, 180, 226, 19, 3, "Holiday Dates:",  LEFT, -105, 5, 0, LEFT, 0, 0, ""

         BUTTON, 10388, 10388, 0, 1, 94, 11668, STD, 125, 263, 23, 70, 3, "Insert", "Insert holiday before the currently highlighted holiday in the list"
         BUTTON, 10391, 10391, 0, 1, 93, 11668, STD, 203, 263, 23, 70, 3,    "Add", "Add holiday onto end of holiday list"
         BUTTON, 10389, 10389, 0, 1, 95, 11668, STD, 281, 263, 23, 70, 3, "Remove", "Remove the currently highlighted holiday from the list"
      ENDCASE


 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Site Parameters - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; DATAWIN, 2000, 10000, 1, LOCATE, 160, -1
 MODTABDLG, 3025, 10326, 1, 30, 30, 330, 520, 0, SITE-PARAMETERS, "Site Properties", NOTIMP, 0, NOTIMP, 0
    
    ;*****************************************
    ; Site Parameters - Ground Temperatures Page
    ;*****************************************
    TABPAGE, 3202, 10326, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 12470, 10326,   0, 1, SITE-PARAMETERS, 0,              NAME, -1, STD, 140,  10,  23, 220, 32, 3,          "Site Name:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Name of site"

; AFR 6/23/09 - the following display for non-LEED   compliance flags 1(3)=>7
      COMBO, 14857, 14857,   0, 1, SITE-PARAMETERS, 0,           C-STATE, -1, STD, 140,  50, 300, 220, 19, 7,              "State:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The state where the project is located"
      COMBO, 14858, 14858,   0, 1, SITE-PARAMETERS, 0,          C-REGION, -1, STD, 140,  75, 300, 220, 19, 7,    "Region / County:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The county where the project is located"
; AFR 6/23/09 - the following display for LEED   compliance flags 1(3)=>6
      COMBO, 18990, 18990,   0, 1, SITE-PARAMETERS, 0,         C-COUNTRY, -1, STD, 140,  50, 300, 220, 19, 6,            "Country:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The country where the project is located"
      COMBO, 14857, 14857,   0, 1, SITE-PARAMETERS, 0,           C-STATE, -1, STD, 140,  75, 300, 220, 19, 6,              "State:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The state where the project is located"

; SAC 8/26/09 - added separate C-901-LOCATION combobox
      COMBO, 14859, 14859,   0, 1, SITE-PARAMETERS, 0,        C-LOCATION, -1, STD, 140, 100, 300, 220, 19, 7,    "City / Location:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The discrete location (i.e. city, town, military base, airport) corresponding to design weather and geographic data"
      COMBO, 19045, 19045,   0, 1, SITE-PARAMETERS, 0,    C-901-LOCATION, -1, STD, 140, 100, 300, 220, 19, 6,    "City / Location:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The discrete location (i.e. city, town, military base, airport) corresponding to design weather and geographic data"

       EDIT, 12535, 12535, 788, 1, SITE-PARAMETERS, 0,          ALTITUDE, -1, STD, 140, 135,  23,  65,  0, 3,           "Altitude:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "Building site altitude above mean sea level, used to adjust air quantities"
; SAC 11/22/10 - added combo to provide access to new D2-DS SPECIFY-AIRFLOWS keyword
      COMBO, 19206, 19206,   0, 1, SITE-PARAMETERS, 0,  SPECIFY-AIRFLOWS, -1, STD, 140, 160,  80, 101, 19, 3, "Airflow Conditions:",  LEFT, -120, 5, 0, LEFT, 4, 5, "Specifies whether HVAC airflows are user-specified at sea-level or at the actual building altitude"
       EDIT, 12504, 12504, 758, 1, SITE-PARAMETERS, 0,          LATITUDE, -1, STD, 140, 185,  23,  65,  2, 3,           "Latitude:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "Building site latitude - northern hemishpere is positive"
       EDIT, 12505, 12505, 758, 1, SITE-PARAMETERS, 0,         LONGITUDE, -1, STD, 140, 210,  23,  65,  2, 3,          "Longitude:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "Building site longitude - degrees from the prime meridian"
;      COMBO, 12534, 12534,   0, 1, SITE-PARAMETERS, 0,  DAYLIGHT-SAVINGS, -1, STD, 140, 210,  80,  81, 19, 3,   "Daylight Savings:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Is daylight savings observed? (Yes/No)"
       EDIT, 14862, 14862,   0, 1, SITE-PARAMETERS, 0,    C-WEATHER-FILE, -1, STD, 140, 235,  23, 182, 32, 1,       "Weather File:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The simulation weather file"

       EDIT, 12506, 12506,   0, 1, SITE-PARAMETERS, 0,         TIME-ZONE, -1, STD, 420, 135,  23,  60,  0, 3,          "Time Zone:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Building site time zone - number of time zones west (+) or east (-) of the prime meridian"
; SAC 11/22/10 - moved daylt sav combo over to right column to make room for D2-DS SPECIFY-AIRFLOWS keyword
      COMBO, 12534, 12534,   0, 1, SITE-PARAMETERS, 0,  DAYLIGHT-SAVINGS, -1, STD, 420, 160,  80,  76, 19, 3,   "Daylight Savings:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Is daylight savings observed? (Yes/No)"
; AFR 6/23/09 - the following display for non-LEED   compliance flags 1(3)=>7
       EDIT, 14860, 14860,   0, 1, SITE-PARAMETERS, 0,    C-CLIMATE-ZONE, -1, STD, 420, 185,  23,  60,  0, 7,       "Climate Zone:",  LEFT, -100, 5, 0, LEFT, 4, 5, "The compliance ruleset climate zone for determining budget requirements"
       EDIT, 14861, 14861,   0, 1, SITE-PARAMETERS, 0,  C-CLIMATE-REGION, -1, STD, 420, 210,  23,  60,  0, 7,     "Climate Region:",  LEFT, -100, 5, 0, LEFT, 4, 5, "The compliance ruleset compliance region for determining envelope requirements"
; AFR 6/23/09 - the following display for LEED   compliance flags 1(3)=>6
      COMBO, 18991, 18991,   0, 1, SITE-PARAMETERS, 0,   C-901-CZ-NUMBER, -1, STD, 420, 185, 200,  60, 19, 6, "Climate Zone Number:", LEFT, -135, 5, 0, LEFT, 4, 5, "The ASHRAE climate zone number for the project"
      COMBO, 18992, 18992,   0, 1, SITE-PARAMETERS, 0,   C-901-CZ-LETTER, -1, STD, 420, 210, 200,  60, 19, 6, "Climate Zone Letter:", LEFT, -123, 5, 0, LEFT, 4, 5, "The ASHRAE climate zone letter for the project"


;     BUTTON, 10275, 10275,   0, 1, 92, 3197, STD, 170, 132, 21,  90, 3, "Design Day", ""

; TESTING  TESTING  TESTING  TESTING  TESTING 
; TESTING  TESTING  TESTING  TESTING  TESTING 
; TESTING  TESTING  TESTING  TESTING  TESTING 
;      BUTTON, 12535, 12535, 0, 1, 92, 3157, STD,  20, 240, 23,  80, 3, "A-Sch", ""
;      BUTTON, 12504, 12504, 0, 1, 92, 3159, STD, 120, 240, 23,  80, 3, "W-Sch", ""
;      BUTTON, 12505, 12505, 0, 1, 92, 3161, STD, 220, 240, 23,  80, 3, "D-Sch", ""
;
;      BUTTON, 12506, 12506, 0, 1, 92, 3069, STD,  20, 270, 23,  80, 3, "Loop", ""
;      BUTTON, 14860, 14860, 0, 1, 92, 3137, STD, 120, 270, 23,  80, 3, "Mat", ""
;      BUTTON, 14861, 14861, 0, 1, 92, 3017, STD, 220, 270, 23,  80, 3, "Door", ""
; TESTING  TESTING  TESTING  TESTING  TESTING 
; TESTING  TESTING  TESTING  TESTING  TESTING 
; TESTING  TESTING  TESTING  TESTING  TESTING 

    ;*****************************************
    ; Site Parameters - Ground Temperatures Page
    ;*****************************************
    TABPAGE, 3026, 10326, 1, 3, NOTIMP, " Ground Temps "

     SPREAD, 11502, 11502, 0, 1, 0, PowerDOE, 0, SiteGrndTemp,  0, STD, 150, 15, 260, 221, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, "average monthly ground temperatures"
    
    ;*****************************************
    ; Site Parameters - Solar/Daylighting Page
    ;*****************************************
    TABPAGE, 3027, 11503, 1, 3, NOTIMP, " Solar - Daylighting "

     SPREAD, 11503, 11503, 0, 1, 0, PowerDOE, 0, SiteSolar,  0, STD,    55,  15, 260, 406, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, "solar and daylighting site parameters"
    
    ;*****************************************
    ; Site Parameters - Terrain Page
    ;*****************************************
    TABPAGE, 3028, 3028, 1, 3, NOTIMP, " Terrain "

     SPREAD, 11504, 11504, 0, 1, 0, PowerDOE, 0, SiteTerrain,  0, STD,  20,  15, 260, 206, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, "site terrain parameters - used to adjust wind speed from weather station to site conditions"
     
       EDIT, 12536, 12536, 773, 1,  SITE-PARAMETERS, 0,  SHIELDING-COEF, -1, STD, 410,  75, 23, 60,  2, 3,   "Shielding Coefficient:",  LEFT, -145, 5, 0, LEFT, 4, 5, ""
       EDIT, 12537, 12537, 773, 1,  SITE-PARAMETERS, 0,    TERRAIN-PAR1, -1, STD, 410, 100, 23, 60,  2, 3,     "Terrain Parameter 1:",  LEFT, -145, 5, 0, LEFT, 4, 5, "Building site terrain parameter; used to convert wind speed from weather station conditions"
       EDIT, 12538, 12538, 773, 1,  SITE-PARAMETERS, 0,    TERRAIN-PAR2, -1, STD, 410, 125, 23, 60,  2, 3,     "Terrain Parameter 2:",  LEFT, -145, 5, 0, LEFT, 4, 5, "Building site terrain parameter; used to convert wind speed from weather station conditions"
       EDIT, 12539, 12539, 773, 1,  SITE-PARAMETERS, 0, WS-TERRAIN-PAR1, -1, STD, 410, 150, 23, 60,  2, 3,   "Weather Station Par 1:",  LEFT, -145, 5, 0, LEFT, 4, 5, "Weather station terrain parameter; used to convert wind speed from weather station to site"
       EDIT, 12540, 12540, 773, 1,  SITE-PARAMETERS, 0, WS-TERRAIN-PAR2, -1, STD, 410, 175, 23, 60,  2, 3,   "Weather Station Par 2:",  LEFT, -145, 5, 0, LEFT, 4, 5, "Weather station terrain parameter; used to convert wind speed from weather station to site"
       EDIT, 12541, 12541, 773, 1,  SITE-PARAMETERS, 0,       WS-HEIGHT, -1, STD, 410, 200, 23, 60,  0, 3,  "Weather Station Height:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Height above ground at which wind speed data were recorded"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Building Parameters - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; DATAWIN, 2001, 10027, 1, BLDG_3D, 110, -1
 MODTABDLG, 3203, 3203, 1, 30, 30, 380, 420, 0, BUILD-PARAMETERS, "Building Properties", NOTIMP, 0, NOTIMP, 0

    ;******************************************************
    ; Building - Daylighting / Solar Page
    ;******************************************************
    TABPAGE, 3204, 3204, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 12436,  3156,   0, 1, BUILD-PARAMETERS,  0,             NAME, -1, STD, 165,  10,  23, 155, 32, 3,     "Building Name:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "Name of building"

      LABEL, "Location, Orientation & Size", STD, LEFT, 70,  53, 0, 0, 1, 320, 12549, 3
       EDIT, 12549, 12549, 757, 1, BUILD-PARAMETERS,  0,            X-REF, -1, STD, 220,  75,  23,  80,  1, 3,       "X-Reference:",  LEFT, -135, 5, 1, LEFT, 4, 5, "X coordinate for the building origin (relative to the Reference coordinate system)"
       EDIT, 12550, 12550, 757, 1, BUILD-PARAMETERS,  0,            Y-REF, -1, STD, 220, 100,  23,  80,  1, 3,       "Y-Reference:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Y coordinate for the building origin (relative to the Reference coordinate system)"
       EDIT, 12542, 12542, 757, 1, BUILD-PARAMETERS,  0,          AZIMUTH, -1, STD, 220, 125,  23,  80,  1, 3,           "Azimuth:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Azimuth relative to true north (positive for clockwise rotation)"
       EDIT, 12544, 12544,   0, 1, BUILD-PARAMETERS,  0,       GROSS-AREA, -1, STD, 220, 150,  23,  80,  0, 3,        "Gross Area:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Total building gross area (equals or exceeds sum of areas for conditioned spaces)"

      LABEL, "Peak Periods & Holidays", STD, LEFT, 70, 198, 0, 0, 1, 320, 12545, 3
       EDIT, 12545, 12545,   0, 1, BUILD-PARAMETERS,  0, HEAT-PEAK-PERIOD,  0, STD, 220, 220,  23,  30,  0, 3,  "Heat Peak Period:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Starting hour of daily time interval used to calculate Design Day heating peak loads"
       EDIT, 12546, 12545,   0, 1, BUILD-PARAMETERS,  0, HEAT-PEAK-PERIOD,  1, STD, 270, 220,  23,  30,  0, 3,                  "-", RIGHT,   -8, 5, 1, LEFT, 4, 5, "Ending hour of daily time interval used to calculate Design Day heating peak loads"
       EDIT, 12547, 12547,   0, 1, BUILD-PARAMETERS,  0, COOL-PEAK-PERIOD,  0, STD, 220, 245,  23,  30,  0, 3,  "Cool Peak Period:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Starting hour of daily time interval used to calculate Design Day cooling peak loads"
       EDIT, 12548, 12547,   0, 1, BUILD-PARAMETERS,  0, COOL-PEAK-PERIOD,  1, STD, 270, 245,  23,  30,  0, 3,                  "-", RIGHT,   -8, 5, 1, LEFT, 4, 5, "Ending hour of daily time interval used to calculate Design Day cooling peak loads"

     COMBO,  12543, 12543,   0, 1, BUILD-PARAMETERS,  0,         HOLIDAYS, -1, STD, 150, 270, 220, 170, 19, 3,          "Holidays:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "Whether Holidays follow different schedules than days of the week (Mondays, Tuesdays, etc.)"
     BUTTON, 10390, 10390,   0, 1, 92, 3215, STD, 220, 297, 23, 100, 3, "Holidays", "Select to edit/view holidays data."

;     EDIT,  12551, 12551,   0, 1,  BUILD-PARAMETERS,  0,  SOLAR-REFL-CALC, -1, STD, 210, 185,  21,  50,  0, 3, "Solar Reflectance Calculation:",  RIGHT, 195, 187, 0, LEFT, 265, 187, "Do you wish to calculate detailed solar reflections from adjacent components? (Yes/No)"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Building/Fixed Shade - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; DATAWIN, 2001, 10027, 1, BLDG_3D, 110, -1
 MODTABDLG, 3205, 32005, 1, 30, 30, 370, 570, 0, NOTIMP, "Building and Fixed Shade Properties", NOTIMP, 0, NOTIMP, 0

   ;******************************************
   ;  Building Shade Tab
   ;******************************************
   TABPAGE, 3206, 32005, 1, 3, BUILDING-SHADE, " Building Shade "
 
      COMBO, 12491, 12491,     0, 1,  BUILDING-SHADE, 0,           NAME,  0, STD, 250,   5, 400, 200, 19, 3, "Currently Active Building Shade:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all building shades defined in project; also allows library retrieval and creation"

       LINE,  20, 40, 545, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

       EDIT, 12552, 12552, 32005, 1,  BUILDING-SHADE, 0,           NAME, -1, STD, 125,  65,  23, 200, 32, 3,       "Building Shade:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "Name of building shade; right mouse quick menu options allow deleting, copying, linking and saving to library"

      COMBO, 12015,   679, 32005, 1,  BUILDING-SHADE, 0, SHADE-SCHEDULE, -1, STD, 125,  95, 250, 200, 19, 3,             "Schedule:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""

      LABEL, "Location & Geometry", STD, LEFT, 30, 138, 0, 0, 1, 310, 0, 3
       EDIT, 19080, 19080,   788, 1,  BUILDING-SHADE, 0,              X, -1, STD,  55, 160,  23,  60,  1, 3,                    "X:",  LEFT,  -25, 5, 1, LEFT, 4, 5, "X coordinate for the shade origin (relative to the Building coordinate system)"
       EDIT, 19081, 19081,   788, 1,  BUILDING-SHADE, 0,              Y, -1, STD,  55, 185,  23,  60,  1, 3,                    "Y:",  LEFT,  -25, 5, 1, LEFT, 4, 5, "Y coordinate for the shade origin (relative to the Building coordinate system)"
       EDIT, 19082, 19082,   788, 1,  BUILDING-SHADE, 0,              Z, -1, STD,  55, 210,  23,  60,  1, 3,                    "Z:",  LEFT,  -25, 5, 1, LEFT, 4, 5, "Z coordinate for the shade origin (relative to the Building coordinate system)"

       EDIT, 19083, 19083, 32005, 1,  BUILDING-SHADE, 0,         HEIGHT, -1, STD, 225, 160,  23,  60,  1, 3,               "Height:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Height of the shade (measured parallel to the Building z-axis)."
       EDIT, 19084, 19084, 32005, 1,  BUILDING-SHADE, 0,          WIDTH, -1, STD, 225, 185,  23,  60,  1, 3,                "Width:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Width of the shade (measured parallel to the Building x-axis)."
       EDIT, 19085, 19085,   788, 1,  BUILDING-SHADE, 0,        AZIMUTH, -1, STD, 225, 210,  23,  60,  1, 3,              "Azimuth:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Azimuth of surface outward normal relative to Building Y-axis (positive = clockwise rotation)"
       EDIT, 19087, 19087, 32005, 1,  BUILDING-SHADE, 0,           TILT, -1, STD, 225, 235,  23,  60,  1, 3,                 "Tilt:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Tilt of the surface outward normal"

      LABEL, "Solar Properties", STD, LEFT, 360, 138, 0, 0, 1, 535, 0, 3
       EDIT, 12560, 12560, 32005, 1,  BUILDING-SHADE, 0,  TRANSMITTANCE, -1, STD, 485, 160,  23,  50,  2, 3,        "Transmittance:",  LEFT, -125, 5, 1, LEFT, 4, 5, ""
       EDIT, 12561, 12561,  3006, 1,  BUILDING-SHADE, 0, SHADE-VIS-REFL, -1, STD, 485, 185,  23,  50,  2, 3,  "Visible Reflectance:",  LEFT, -125, 5, 1, LEFT, 4, 5, ""
       EDIT, 12562, 12562, 32005, 1,  BUILDING-SHADE, 0, SHADE-GND-REFL, -1, STD, 485, 210,  23,  50,  2, 3,   "Ground Reflectance:",  LEFT, -125, 5, 1, LEFT, 4, 5, ""
       COMBO,19329, 19329,     0, 1,  BUILDING-SHADE, 0,          SHAPE, -1, STD, 100, 275, 120, 275, 19, 3,             "Shape:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Rectangle Or Polygon"
       COMBO,19330, 19330, 31030, 1,  BUILDING-SHADE, 0,        POLYGON, -1, STD, 100, 300, 220, 275, 19, 3,           "Polygon:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Name of the Polygon that defines the building shade's shape"

   ;******************************************
   ;  Fixed Shade Tab
   ;******************************************
   TABPAGE, 3207, 32005, 1, 3, FIXED-SHADE, " Fixed Shade "
 
      COMBO, 12497, 12497,     0, 1,  FIXED-SHADE, 0,          NAME,  0, STD, 250,   5, 400, 200, 19, 3, "Currently Active Fixed Shade:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all fixed shades defined in project; also allows library retrieval and creation"

       LINE,  20, 40, 545, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

       EDIT, 12800, 12800, 32005, 1,  FIXED-SHADE, 0,           NAME, -1, STD, 125,  65,  23, 200, 32, 3,          "Fixed Shade:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "Name of fixed shade; right mouse quick menu options allow deleting, copying, linking and saving to library"

      COMBO, 12016, 19094, 32005, 1,  FIXED-SHADE, 0, SHADE-SCHEDULE, -1, STD, 125,  95, 250, 200, 19, 3,             "Schedule:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""

      LABEL, "Location & Geometry", STD, LEFT, 30, 138, 0, 0, 1, 310, 0, 3
       EDIT, 19088, 19088,   788, 1,  FIXED-SHADE, 0,          X-REF, -1, STD,  55, 160,  23,  60,  1, 3,                    "X:",  LEFT,  -25, 5, 1, LEFT, 4, 5, "X coordinate for the shade origin (relative to the Site coordinate system)"
       EDIT, 19089, 19089,   788, 1,  FIXED-SHADE, 0,          Y-REF, -1, STD,  55, 185,  23,  60,  1, 3,                    "Y:",  LEFT,  -25, 5, 1, LEFT, 4, 5, "Y coordinate for the shade origin (relative to the Site coordinate system)"
       EDIT, 19090, 19090,   788, 1,  FIXED-SHADE, 0,          Z-REF, -1, STD,  55, 210,  23,  60,  1, 3,                    "Z:",  LEFT,  -25, 5, 1, LEFT, 4, 5, "Z coordinate for the shade origin (relative to the Site coordinate system)"

       EDIT, 19091, 19091, 32005, 1,  FIXED-SHADE, 0,         HEIGHT, -1, STD, 225, 160,  23,  60,  1, 3,               "Height:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Height of the shade (measured parallel to the Site z-axis)."
       EDIT, 19092, 19092, 32005, 1,  FIXED-SHADE, 0,          WIDTH, -1, STD, 225, 185,  23,  60,  1, 3,                "Width:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Width of the shade (measured parallel to the Site x-axis)."
       EDIT, 19093, 19093,   788, 1,  FIXED-SHADE, 0,        AZIMUTH, -1, STD, 225, 210,  23,  60,  1, 3,              "Azimuth:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Azimuth of surface outward normal relative to Site Y-axis (positive = clockwise rotation)"
       EDIT, 19095, 19095, 32005, 1,  FIXED-SHADE, 0,           TILT, -1, STD, 225, 235,  23,  60,  1, 3,                 "Tilt:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Tilt of the surface outward normal"

      LABEL, "Solar Properties", STD, LEFT, 360, 138, 0, 0, 1, 535, 0, 3
       EDIT, 12801, 12801, 32005, 1,  FIXED-SHADE, 0,  TRANSMITTANCE, -1, STD, 485, 160,  23,  50,  2, 3,        "Transmittance:",  LEFT, -125, 5, 1, LEFT, 4, 5, ""
       EDIT, 12802, 12802,  3006, 1,  FIXED-SHADE, 0, SHADE-VIS-REFL, -1, STD, 485, 185,  23,  50,  2, 3,  "Visible Reflectance:",  LEFT, -125, 5, 1, LEFT, 4, 5, ""
       EDIT, 12803, 12803, 32005, 1,  FIXED-SHADE, 0, SHADE-GND-REFL, -1, STD, 485, 210,  23,  50,  2, 3,   "Ground Reflectance:",  LEFT, -125, 5, 1, LEFT, 4, 5, ""

       COMBO, 19331, 19331,     0, 1, FIXED-SHADE, 0,          SHAPE, -1, STD, 100, 275, 120, 275, 19, 3,             "Shape:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Rectangle Or Polygon"
       COMBO, 19332, 19332, 31030, 1, FIXED-SHADE, 0,        POLYGON, -1, STD, 100, 300, 220, 275, 19, 3,           "Polygon:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Name of the Polygon that defines the fixed shade's shape"


 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Floor - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; DATAWIN, 2019, 1510, 1, BLDG_FLR, 135, -1
; AFR 6/23/09 - changed height from 440 to 470
 MODTABDLG, 3208, 1510, 1, 30, 30, 470, 420, 0, FLOOR, "Floor Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 12429,  1510, 0, 1, FLOOR, 0, NAME,  0, STD, 155, 15, 400, 250, 19, 3, "Currently Active Floor:",  LEFT, -140, 5, 0, LEFT, 4, 5, "List of all floors defined in project; also allows library retrieval and creation"

    ;******************************************
    ; Floor - Basic Specs Page
    ;******************************************
    TABPAGE, 3209, 1510, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 12318,  1003,     0, 1,  FLOOR, 0,             NAME, -1, STD, 115,  10,  23, 260, 32, 3,        "Floor Name:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Name of floor; right mouse quick menu options allow deleting, copying, linking and saving to library"

       EDIT, 12422, 12422,   769, 1,  FLOOR, 0,       MULTIPLIER, -1, STD, 115,  40,  23,  50,  0, 3,        "Multiplier:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Number of floors in the facility that are identical, and served by the same HVAC system"
       
; AFR 6/24/09 - added for LEED
      COMBO, 18993, 18993,     0, 1,  FLOOR, 0,  C-901-BLDG-TYPE, -1, STD, 115,  70, 120, 275, 19, 6,     "Building Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "ASHRAE building type for floor"
      COMBO, 18994, 18994, 31030, 1,  FLOOR, 0,  C-HTG-SYS-CLASS, -1, STD, 115,  95, 220, 275, 19, 6,    "Heating Source:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Heating source type for floor"
      
; AFR 6/24/09 - moved everything below here down a bit for extra room to accomodate the two LEED combo boxes      
      LABEL, "Geometry", STD, LEFT, 40, 128, 0, 0, 1, 375, 0, 3
      COMBO, 19166, 19166,     0, 1,  FLOOR, 0,            SHAPE, -1, STD, 100, 150, 120, 275, 19, 3,             "Shape:",  LEFT,  -60, 5, 0, LEFT, 4, 5, ""
      COMBO, 19060, 19060, 31030, 1,  FLOOR, 0,          POLYGON, -1, STD, 100, 175, 220, 275, 19, 3,           "Polygon:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Name of the Polygon that defines the floor's shape"

       EDIT, 19026,  1002,   788, 1,  FLOOR, 0,                X, -1, STD, 100, 200,  23,  60,  2, 3,                 "X:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "X coordinate for the floor origin (relative to the Building coordinate system)"
       EDIT, 19048, 19048,   788, 1,  FLOOR, 0,                Y, -1, STD, 100, 225,  23,  60,  2, 3,                 "Y:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Y coordinate for the floor origin (relative to the Building coordinate system)"
       EDIT, 19049, 19049,   788, 1,  FLOOR, 0,                Z, -1, STD, 100, 250,  23,  60,  2, 3,                 "Z:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Z coordinate for the floor origin (relative to the Building coordinate system)"
       EDIT, 19059, 19059,   788, 1,  FLOOR, 0,          AZIMUTH, -1, STD, 100, 275,  23,  60,  2, 3,           "Azimuth:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Azimuth of outward normal relative to Building Y-axis; before applying Tilt (positive = clockwise)"

       EDIT, 19168, 19168,     0, 1,  FLOOR, 0,     FLOOR-HEIGHT, -1, STD, 300, 200,  23,  59,  2, 3,     "Flr-to-Flr Ht:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Height of floor: used only, and required, if the floor is defined with either Shape=BOX or Polygon"
       EDIT, 19167, 19167,     0, 1,  FLOOR, 0,     SPACE-HEIGHT, -1, STD, 300, 225,  23,  59,  2, 3,     "Flr-to-Clg Ht:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Default height for spaces assigned to this floor"
       EDIT, 19170, 19170,     0, 1,  FLOOR, 0,            WIDTH, -1, STD, 300, 250,  23,  59,  2, 3,             "Width:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Applies (& required) only if the floor is defined via Shape=BOX"
       EDIT, 19169, 19169,     0, 1,  FLOOR, 0,            DEPTH, -1, STD, 300, 275,  23,  59,  2, 3,             "Depth:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Applies (& required) only if the floor is defined via Shape=BOX"
       EDIT, 12279, 12279,     0, 1,  FLOOR, 0,             AREA, -1, STD, 275, 300,  23,  85,  0, 3,              "Area:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Area of this floor (before multiplication by Floor Multiplier)"
       EDIT, 12280, 12280,     0, 1,  FLOOR, 0,           VOLUME, -1, STD, 275, 325,  23,  85,  0, 3,            "Volume:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Air volume of this floor (before multiplication by Floor Multiplier)"

; SAC 10/23/00 - Compliance keyword
; AFR 6/24/09 - hide for LEED.
       EDIT, 15481,     0,     0, 1,  FLOOR, 0,  C-DISPLAY-PERIM, -1, STD, 275, 350,  23,  85,  0, 7, "Display Perimeter (compliance):", RIGHT, -5, 5, 1, LEFT, 4, 5, "The display perimeter on this building floor"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Space - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; MODTABDLG, 3000, 10031, 1, 100, 100, 300, 600, 0, "Zone Properties:   ", SPACE, 0, NAME, -1, 32, 0, "", NOTIMP, 0, NOTIMP, 0
; MODTABDLG, 3000, 10031, 1, 30, 30, 470, 710, 0, SPACE, "Space Properties", NOTIMP, 0, NOTIMP, 0
; AFR 5/12/09 - increased dialog size from 470 x 710 to 570 x 1030.
 MODTABDLG, 3000, 10031, 1, 30, 30, 570, 1030, 0, SPACE, "Space Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 12399, 10031, 0, 1, SPACE, 0, NAME,  0, STD, 215,  15, 400, 250, 19, 3, "Currently Active Space:",  LEFT, -150, 5, 0, LEFT, 4, 5, "List of all spaces defined in project; also allows library retrieval and creation"
   STATIC, 1, SPACE, 0, ZONE-TYPE, 0, 0, 0, 485, 20, 250, STD, LEFT, "Zone Type: ",   "", 0, 3

    ;******************************************
    ; Space - Basic Specs Page
    ;******************************************
    TABPAGE, 3210, 10031, 1, 3, NOTIMP, " Basic Specs "

; Left side of the screen
       EDIT, 12000, 12000,     0, 1,  SPACE, 0,             NAME, -1, STD, 105,   5,  23, 235, 32, 3,        "Space Name:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Name of space; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 15620, 15620,     0, 1,  SPACE, 0,           PARENT, -1, STD, 105,  30, 100, 235, 19, 3,      "Parent Floor:",  LEFT,  -85, 5, 0, LEFT, 4, 5, ""
      COMBO, 12169, 12263,     0, 1,  SPACE, 0,        ZONE-TYPE, -1, STD, 105,  55, 100, 235, 19, 3,         "Zone Type:",  LEFT,  -85, 5, 0, LEFT, 4, 5, ""
; SAC 7/19/03 - Added to provide user access to field used in system/zone summary QC report
       EDIT, 17780,     0,     0, 1,  SPACE, 0,  C-ACTIVITY-DESC, -1, STD, 105,  80,  23, 235, 32, 3,       "Description:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Description of space usage"
      LABEL, "Multipliers:", STD, LEFT,  20, 110, 0, 0, 1, 0, 0, 3
       EDIT, 12002, 12002,   769, 1,  SPACE, 0,       MULTIPLIER, -1, STD, 155, 105,  23,  50,  0, 3,             "Space:", RIGHT,   -7, 5, 0, LEFT, 4, 5, ""
       EDIT, 12003, 12422,   769, 1,  SPACE, 0, FLOOR-MULTIPLIER, -1, STD, 275, 105,  23,  50,  0, 3,             "Floor:", RIGHT,   -7, 5, 0, LEFT, 4, 5, "Number of floors in the facility that are identical, and served by the same HVAC system"
; SAC 10/20/00 - added missing SUNSPACE keyword
      COMBO, 12021, 12021,   753, 1,  SPACE, 0,         SUNSPACE, -1, STD, 105, 130, 100, 100, 19, 3,          "Sunspace:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Sunspaces allow more detailed calculations of heat transfer with other spaces"
; SAC 2/20/02 - added missing TEMPERATURE keyword
       EDIT, 17694, 12022,   752, 1,  SPACE, 0,      TEMPERATURE,  0, STD, 275, 130,  23,  50,  1, 3,             "Temp.:", RIGHT,   -7, 5, 1, LEFT, 4, 5, "Annual average space T: normally set this to midpoint of Heating & Cooling Design T's"

      LABEL, "Location & Geometry", STD, LEFT, 20, 165, 0, 0, 1, 340, 0, 3
      COMBO, 19155, 19155,     0, 1,  SPACE, 0,         LOCATION, -1, STD,  80, 185, 220, 260, 19, 3,          "Location:",  LEFT,  -60, 5, 0, LEFT, 4, 5, ""
      COMBO, 19004, 19004,   755, 1,  SPACE, 0,            SHAPE, -1, STD,  80, 210, 120, 260, 19, 3,             "Shape:",  LEFT,  -60, 5, 0, LEFT, 4, 5, ""
      COMBO, 19020, 19020, 31030, 1,  SPACE, 0,          POLYGON, -1, STD,  80, 235, 220, 260, 19, 3,           "Polygon:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Name of the Polygon that defines the space's floor geometry"

       EDIT, 19000, 19000,   756, 1,  SPACE, 0,                X, -1, STD,  80, 260,  23,  60,  2, 3,                 "X:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "X coordinate for the space origin (relative to the Floor coordinate system)"
       EDIT, 19001, 19001,   756, 1,  SPACE, 0,                Y, -1, STD,  80, 285,  23,  60,  2, 3,                 "Y:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Y coordinate for the space origin (relative to the Floor coordinate system)"
       EDIT, 19002, 19002,   756, 1,  SPACE, 0,                Z, -1, STD,  80, 310,  23,  60,  2, 3,                 "Z:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Z coordinate for the space origin (relative to the Building coordinate system)"
       EDIT, 19003, 19003,   756, 1,  SPACE, 0,          AZIMUTH, -1, STD,  80, 335,  23,  60,  2, 3,           "Azimuth:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Azimuth of Space Y-axis relative to Building Y-axis (positive = clockwise rotation)"

       EDIT, 19016, 19016,     0, 1,  SPACE, 0,           HEIGHT, -1, STD, 275, 260,  23,  50,  1, 3,     "Flr-to-Clg Ht:",  LEFT,  -80, 5, 1, LEFT, 4, 5, "Height of space: used only, and required, if the space is defined with either Shape or Polygon"
       EDIT, 19006, 19006,     0, 1,  SPACE, 0,            WIDTH, -1, STD, 250, 285,  23,  75,  2, 3,             "Width:",  LEFT,  -55, 5, 1, LEFT, 4, 5, "Applies (& required) only if the space is defined via Shape"
       EDIT, 19005, 19005,     0, 1,  SPACE, 0,            DEPTH, -1, STD, 250, 310,  23,  75,  2, 3,             "Depth:",  LEFT,  -55, 5, 1, LEFT, 4, 5, "Applies (& required) only if the space is defined via Shape"
       EDIT, 12004, 12004,     0, 1,  SPACE, 0,             AREA, -1, STD, 250, 335,  23,  75,  1, 3,              "Area:",  LEFT,  -55, 5, 1, LEFT, 4, 5, "Floor area of this space (before multiplication by Multiplier or Floor Multiplier)"
       EDIT, 12005, 12005,     0, 1,  SPACE, 0,           VOLUME, -1, STD, 250, 360,  23,  75,  0, 3,            "Volume:",  LEFT,  -55, 5, 1, LEFT, 4, 5, "Air volume of this space (before multiplication by Multiplier or Floor Multiplier)"

; AFR 6/24/09 - make all control visible with rule sets are loaded.  Rearrange some controls to fit the screen.
; Right side of the screen
; SAC 11/25/00 - Compliance keywords
      LABEL, "Compliance Settings", STD, LEFT, 390,  10, 0, 0, 1, 1005, 15521, 1
; AFR 6/24/09 - the next three controls only display if the ruleset is non-LEED      
      COMBO, 15521, 15521,     0, 1,  SPACE, 0,   C-CONDITIONING,  0, STD, 500,  30, 220, 175, 19, 7,       "Conditioning:", LEFT, -100, 5, 0, LEFT, 4, 5, "The type of space conditioning"
      COMBO, 15522, 15522,     0, 1,  SPACE, 0,  C-SCHEDULE-TYPE,  0, STD, 500,  55, 220, 175, 19, 7,      "Schedule Type:", LEFT, -100, 5, 0, LEFT, 4, 5, "The type of schedules"
       EDIT, 15596, 15596,     0, 1,  SPACE, 0, C-TRNSFR-AIR-CFM,  0, STD, 500,  80,  23,  80,  2, 7,       "Transfer Air:", LEFT, -100, 5, 1, LEFT, 4, 5, "The quantity of transfer air into (or out of) this space"
   CHECKBOX, 15590, 15590,     0, 1,  SPACE, 0, C-LTG-PLANS-INCL,  0, STD, 405, 108,  17, 275,     7,  "Includes Lighting Plans", RIGHT,                   "Check if lighting plans are included for this space"

; AFR 6/24/09 - the next several controls only display if the ruleset is LEED
      COMBO, 18997, 18997,     0, 1,  SPACE, 0,  C-901-BLDG-TYPE,  0, STD, 500,  30, 220, 175, 19, 6,         "Building Type:", LEFT, -100, 5, 0, LEFT, 4, 5, "ASHRAE building type for space"
      COMBO, 18995, 18995,     0, 1,  SPACE, 0,  C-901-CONDITION,  0, STD, 500,  55, 220, 175, 19, 6,          "Conditioning:", LEFT, -100, 5, 0, LEFT, 4, 5, "The type of space conditioning"
      COMBO, 18996, 18996,     0, 1,  SPACE, 0,  C-901-SCH-TYPE,   0, STD, 500,  80, 220, 175, 19, 6,         "Schedule Type:", LEFT, -100, 5, 0, LEFT, 4, 5, "ASHRAE schedule type"
      
      COMBO, 18998, 18998,     0, 1,  SPACE, 0,  C-HTG-SYS-CLASS,  0, STD, 830,  30, 220, 175, 19, 6,        "Heating Source:", LEFT, -140, 5, 0, LEFT, 4, 5, "Heating source type for space"
      COMBO, 18999, 18999,     0, 1,  SPACE, 0,  C-SYS-EXCEPTION1, 0, STD, 830,  55, 220, 175, 19, 6, "System Type Exception:", LEFT, -140, 5, 0, LEFT, 4, 5, "Appendix G3.1.1 exception for baseline system type"
      COMBO, 19007, 19007,     0, 1,  SPACE, 0,  C-SYS-EXCEPTION2, 0, STD, 830,  80, 220, 175, 19, 6,  "Economizer Exception:", LEFT, -140, 5, 0, LEFT, 4, 5, "Appendix G3.1.2.6 exception for economizer requirement"
      COMBO, 19019, 19019,     0, 1,  SPACE, 0,  C-SYS-EXCEPTION3, 0, STD, 830, 105, 220, 175, 19, 6,         "ERV Exception:", LEFT, -140, 5, 0, LEFT, 4, 5, "Appendix G3.1.2.10 exception for ERV requirement"

;    TABPAGE, 3001, 3001, 1, 3, NOTIMP, " Occupancy "
      LABEL, "Occupancy", STD, LEFT, 390, 165, 0, 0, 1,1005, 0, 3
      COMBO, 12067, 12067,  3001, 1,  SPACE, 0,  PEOPLE-SCHEDULE, -1, STD, 455, 185, 220, 220, 19, 3,           "Schedule:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Name of the schedule that governs occupancy in the selected space"
       EDIT, 12065, 12065,  3001, 1,  SPACE, 0,      AREA/PERSON, -1, STD, 510, 210,  23,  80,  0, 3,        "Area/Person:", LEFT, -120, 5, 1, LEFT, 4, 5, "Maximum occupancy density (expressed as area per person in the selected space)"
       EDIT, 12064, 12064,  3001, 1,  SPACE, 0, NUMBER-OF-PEOPLE, -1, STD, 510, 235,  23,  80,  0, 3,   "Number of People:", LEFT, -120, 5, 1, LEFT, 4, 5, "Maximum number of people in the space"
       EDIT, 12066, 12066,  3001, 1,  SPACE, 0, PEOPLE-HEAT-GAIN, -1, STD, 510, 260,  23,  80,  0, 3,    "Total Heat Gain:", LEFT, -120, 5, 1, LEFT, 4, 5, "Total (sensible plus latent) heat gain per occupant in the selected space"
       EDIT, 12069, 12069,  3001, 1,  SPACE, 0,   PEOPLE-HG-SENS, -1, STD, 510, 285,  23,  80,  0, 3, "Sensible Heat Gain:", LEFT, -120, 5, 1, LEFT, 4, 5, "Sensible heat gain per occupant in the selected space"
       EDIT, 12068, 12068,  3001, 1,  SPACE, 0,    PEOPLE-HG-LAT, -1, STD, 510, 310,  23,  80,  0, 3,   "Latent Heat Gain:", LEFT, -120, 5, 1, LEFT, 4, 5, "Latent heat gain per occupant in the selected space"

; SAC 11/25/00 - Compliance keywords
; AFR 6/24/09 - display for non-LEED
       SPREAD, 11695, 11695, 0, 1, 0, PowerDOE, 0,    SpaceOccTypeSpread,  0, STD, 390, 345, 120, 385, 19, 7, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
; AFR 6/24/09 - display for LEED       
       SPREAD, 11695, 11696, 0, 1, 0, PowerDOE, 0, Space901OccTypeSpread,  0, STD, 390, 345, 120, 285, 19, 6, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
       
      ; SAC 11/9/09 - shortened above spreads 1 row and moved the occup type area sum to be below the 
      ; STATIC, 1, SPACE,  0, C-AREA, -1, 0, 1, 1000, 193, -1, STD, RIGHT, "Sum of Occupancy Type Areas:    ", " ", 1, 1
       STATIC, 1, SPACE,  0, C-AREA, -1, 0, 1,  400, 468, -1, STD,  LEFT, "Sum of Occupancy Type Areas:    ", " ", 1, 1
         
;;    TABPAGE, 3001, 3001, 1, 3, NOTIMP, " Occupancy "
;      LABEL, "Occupancy", STD, LEFT, 390, 165, 0, 0, 1, 775, 0, 3
;      COMBO, 12067, 12067,  3001, 1,  SPACE, 0,  PEOPLE-SCHEDULE, -1, STD, 455, 185, 220, 220, 19, 2,           "Schedule:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Name of the schedule that governs occupancy in the selected space"
;       EDIT, 12065, 12065,  3001, 1,  SPACE, 0,      AREA/PERSON, -1, STD, 510, 210,  23,  80,  0, 2,        "Area/Person:", LEFT, -120, 5, 1, LEFT, 4, 5, "Maximum occupancy density (expressed as area per person in the selected space)"
;       EDIT, 12064, 12064,  3001, 1,  SPACE, 0, NUMBER-OF-PEOPLE, -1, STD, 510, 235,  23,  80,  0, 2,   "Number of People:", LEFT, -120, 5, 1, LEFT, 4, 5, "Maximum number of people in the space"
;       EDIT, 12066, 12066,  3001, 1,  SPACE, 0, PEOPLE-HEAT-GAIN, -1, STD, 510, 260,  23,  80,  0, 2,    "Total Heat Gain:", LEFT, -120, 5, 1, LEFT, 4, 5, "Total (sensible plus latent) heat gain per occupant in the selected space"
;       EDIT, 12069, 12069,  3001, 1,  SPACE, 0,   PEOPLE-HG-SENS, -1, STD, 510, 285,  23,  80,  0, 2, "Sensible Heat Gain:", LEFT, -120, 5, 1, LEFT, 4, 5, "Sensible heat gain per occupant in the selected space"
;       EDIT, 12068, 12068,  3001, 1,  SPACE, 0,    PEOPLE-HG-LAT, -1, STD, 510, 310,  23,  80,  0, 2,   "Latent Heat Gain:", LEFT, -120, 5, 1, LEFT, 4, 5, "Latent heat gain per occupant in the selected space"
;
;; SAC 11/25/00 - Compliance keywords
;      LABEL, "Compliance Settings", STD, LEFT, 390,  10, 0, 0, 1, 675, 15521, 1
;      COMBO, 15521, 15521,     0, 1,  SPACE, 0,   C-CONDITIONING,  0, STD, 500,  30, 220, 175, 19, 1,       "Conditioning:", LEFT, -100, 5, 0, LEFT, 4, 5, "The type of space conditioning"
;      COMBO, 15522, 15522,     0, 1,  SPACE, 0,  C-SCHEDULE-TYPE,  0, STD, 500,  55, 220, 175, 19, 1,      "Schedule Type:", LEFT, -100, 5, 0, LEFT, 4, 5, "The type of schedules"
;       EDIT, 15596, 15596,     0, 1,  SPACE, 0, C-TRNSFR-AIR-CFM,  0, STD, 500,  80,  23,  80,  2, 1,       "Transfer Air:", LEFT, -100, 5, 1, LEFT, 4, 5, "The quantity of transfer air into (or out of) this space"
;   CHECKBOX, 15590, 15590,     0, 1,  SPACE, 0, C-LTG-PLANS-INCL,  0, STD, 405, 108,  17, 275,     1,  "Includes Lighting Plans", RIGHT,                   "Check if lighting plans are included for this space"
;
;; SAC 11/25/00 - Compliance keywords
;       SPREAD, 11695, 11695, 0, 1, 0, PowerDOE, 0,  SpaceOccTypeSpread,  0, STD, 390, 185, 175, 385, 19, 1, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
;         STATIC, 1, SPACE,  0, C-AREA, -1, 0, 1, 670, 363, -1, STD, RIGHT, "Sum of Occupancy Type Areas:    ", " ", 1, 1


    ;******************************************
    ; Space - Equipment Page
    ;******************************************
    TABPAGE, 3002, 3002, 1, 3, NOTIMP, " Equipment "

; SAC 11/22/10 - revised sizes & positions to accommodate EQUIP-TO-RETURN & minimal scrolling
      LABEL, "Equipment", STD, LEFT, 30, 20, 0, 0, 1, 855, 0, 3
       SPREAD, 11692, 11692, 0, 1, 0, PowerDOE, 0,  SpaceEquipSpread,  0, STD, 50, 40, 180, 805, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""

      LABEL, "Internal Energy Sources", STD, LEFT, 30, 260, 0, 0, 1, 675, 0, 3
       SPREAD, 11693, 11693, 0, 1, 0, PowerDOE, 0,  SpaceIntSrcSpread,  0, STD, 50, 280,  80, 625, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
  
    ;******************************************                                                                                                     
    ; Space - Infiltration Page
    ;******************************************
    TABPAGE, 3003, 3003, 1, 3, NOTIMP, " Infiltration "
    
     COMBO, 19138, 12036,   0, 1, SPACE, 0,      INF-METHOD, -1, STD, 150,  15, 120, 150, 19, 3,          "Infiltration Method:",  LEFT, -120, 5, 0, LEFT, 4, 5, "The method DOE-2 uses to calculate the rate of outside air infiltration into the space"
     COMBO, 12037, 12037,   0, 1, SPACE, 0,    INF-SCHEDULE, -1, STD, 400,  15, 220, 200, 19, 3,                     "Schedule:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "A Fraction Schedule that modifies the rate of air infiltration into the space"
      
      LABEL, "Air Change Method", STD, LEFT, 30, 63, 1, 0, 0, 325, 12038, 3
      EDIT, 12038, 12038,   0, 1, SPACE, 0,  AIR-CHANGES/HR, -1, STD, 215,  85,  23,  70,  2, 3,             "Air Changes/Hour:",  LEFT, -170, 5, 0, LEFT, 4, 5, "Number of air changes per hour due to infiltration into the zone, at a wind speed of 10 mph"
      EDIT, 12039, 12039,   0, 1, SPACE, 0,   INF-FLOW/AREA, -1, STD, 215, 110,  23,  70,  4, 3,            "Infiltration Flow:",  LEFT, -170, 5, 1, LEFT, 4, 5, "Outside air infiltration rate into the space per unit floor Area"
    
      LABEL, "Sherman-Grimsrud Method", STD, LEFT, 30, 158, 1, 0, 0, 325, 12045, 3
      EDIT, 12045, 12045, 773, 1, SPACE, 0,   HOR-LEAK-FRAC, -1, STD, 215, 180,  23,  70,  2, 3,        "Horizontal Leak Ratio:",  LEFT, -170, 5, 1, LEFT, 4, 5, "Fraction of the total leakage area that is in the ceiling"
      EDIT, 12046, 12046, 773, 1, SPACE, 0,   NEUTRAL-LEVEL, -1, STD, 215, 205,  23,  70,  2, 3,                "Neutral Level:",  LEFT, -170, 5, 0, LEFT, 4, 5, "Fraction of zone height at which the indoor air pressure equals the outdoor air pressure"
      EDIT, 12047, 12047, 773, 1, SPACE, 0,  FRAC-LEAK-AREA, -1, STD, 215, 230,  23,  70,  2, 3,  "Leak Fraction of Floor Area:",  LEFT, -170, 5, 1, LEFT, 4, 5, "Total leakage area (expressed as a fraction of the floor area of the space)"
      
      LABEL, "Residential", STD, LEFT, 30, 278, 1, 0, 0, 325, 12382, 3
      EDIT, 12382,   674, 674, 1, SPACE, 0,     RES-INF-CST,  0, STD, 215, 300,  23,  70,  2, 3,       "Resid. Infil. Constant:",  LEFT, -170, 5, 0, LEFT, 4, 5, "Used to calculate outside air infiltration into the space (based on wind speed & temperature)"
      EDIT, 12383,   672, 672, 1, SPACE, 0,     RES-INF-WND,  0, STD, 215, 325,  23,  70,  2, 3,           "Resid. Infil. Wind:",  LEFT, -170, 5, 1, LEFT, 4, 5, "Used to calculate outside air infiltration into the space (based on wind speed & temperature)"
      EDIT, 12384,   673, 673, 1, SPACE, 0,    RES-INF-TEMP,  0, STD, 215, 350,  23,  70,  2, 3,    "Resid. Infil. Temperature:",  LEFT, -170, 5, 1, LEFT, 4, 5, "Used to calculate outside air infiltration into the space (based on wind speed & temperature)"
      
      LABEL, "Crack Method", STD, LEFT, 395, 63, 1, 0, 0, 675, 12040, 3
      EDIT, 12040, 12040, 773, 1, SPACE, 0, NEUTRAL-ZONE-HT, -1, STD, 565,  85,  23,  70,  2, 3,          "Neutral Zone Height:",  LEFT, -155, 5, 1, LEFT, 4, 5, "Vertical distance between each zone and the neutral pressure level of the building"

; SAC 3/11/09 - added access to new ASHRAE enhanced infiltration method inputs (and shifted around everything else on this screen to accommodate them)
      LABEL, "ASHRAE Enhanced Method", STD, LEFT, 395, 133, 1, 0, 0, 675, 18985, 3
      EDIT, 18985,     0,   0, 1, SPACE, 0,       FLOW-COEF,  0, STD, 565, 155,  23,  70,  1, 3,             "Flow Coefficient:",  LEFT, -155, 5, 1, LEFT, 4, 5, "Flow Coefficient used in ASHRAE Enhanced Infiltration calculations"
      EDIT, 18986,     0,   0, 1, SPACE, 0,      STACK-COEF,  0, STD, 565, 180,  23,  70,  6, 3,            "Stack Coefficient:",  LEFT, -155, 5, 1, LEFT, 4, 5, "Stack Coefficient used in ASHRAE Enhanced Infiltration calculations"
      EDIT, 18987,     0,   0, 1, SPACE, 0,       WIND-COEF,  0, STD, 565, 205,  23,  70,  6, 3,             "Wind Coefficient:",  LEFT, -155, 5, 1, LEFT, 4, 5, "Wind Coefficient used in ASHRAE Enhanced Infiltration calculations"
      EDIT, 18988,     0,   0, 1, SPACE, 0,  SHELTER-FACTOR,  0, STD, 565, 230,  23,  70,  3, 3,               "Shelter Factor:",  LEFT, -155, 5, 1, LEFT, 4, 5, "Shelter Factor used in ASHRAE Enhanced Infiltration calculations"
      EDIT, 18989,     0,   0, 1, SPACE, 0,    PRESSURE-EXP,  0, STD, 565, 255,  23,  70,  3, 3,            "Pressure Exponent:",  LEFT, -155, 5, 1, LEFT, 4, 5, "Pressure Exponent used in ASHRAE Enhanced Infiltration calculations"

    ;******************************************
    ; Space - Daylighting Page
    ;******************************************
    TABPAGE, 3006, 3006, 1, 3, NOTIMP, " Daylighting "
      
      COMBO, 12048, 12048,    0, 1, SPACE, 0,      DAYLIGHTING, -1, STD, 145,   5,  80,  50, 19, 3,               "Daylighting:",  LEFT, -125, 5, 0, LEFT, 4, 5, "Whether Daylighting is used to supplement electric lighting in this zone"
      COMBO, 12061, 12061, 3006, 1, SPACE, 0, DAYLIGHT-REP-SCH, -1, STD, 145,  30, 220, 200, 19, 3,           "Report Schedule:",  LEFT, -115, 5, 0, LEFT, 4, 5, "An On-Off Schedule that indicates which hours are included in the daylighting reports"

;      LABEL, "Discomfort Glare", STD, LEFT, 50, 158, 1, 0, 0, 265, 12055, 3
;       EDIT, 12055, 12055,  762, 1, SPACE, 0,        MAX-GLARE, -1, STD, 165, 180,  23,  70,  0, 3,             "Maximum Glare:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Maximum tolerable glare before glare control shading devices are deployed"
;       EDIT, 12086, 63035, 3006, 1, SPACE, 0,     VIEW-AZIMUTH, -1, STD, 165, 205,  23,  70,  1, 3,              "View Azimuth:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Direction of the occupant's view (in horizontal plane) in which the daylight glare is calculated"
;
;      LABEL, "Lighting Control", STD, LEFT, 405, 108, 1, 0, 0, 655, 12056, 3
;       EDIT, 12056, 12056, 3006, 1, SPACE, 0,   MIN-POWER-FRAC, -1, STD, 555, 130,  23,  70,  2, 3,    "Minimum Power Fraction:",  LEFT, -150, 5, 1, LEFT, 4, 5, "The minimum input power required by a continuous dimming lighting controller"
;       EDIT, 12057, 12057, 3006, 1, SPACE, 0,   MIN-LIGHT-FRAC, -1, STD, 555, 155,  23,  70,  2, 3,    "Minimum Light Fraction:",  LEFT, -150, 5, 1, LEFT, 4, 5, "The minimum light output achieved by a continuous dimming lighting controller"
;       EDIT, 12058, 12058, 3006, 1, SPACE, 0, LIGHT-CTRL-STEPS, -1, STD, 555, 180,  23,  70,  0, 3,       "Light Control Steps:",  LEFT, -150, 5, 1, LEFT, 4, 5, "The number of steps in a stepped lighting control system (excluding the off state)"
;       EDIT, 12060, 12060, 3006, 1, SPACE, 0,  LIGHT-CTRL-PROB, -1, STD, 555, 205,  23,  70,  2, 3, "Light Control Probability:",  LEFT, -150, 5, 1, LEFT, 4, 5, "Probability of manually switched lights being switched in response to daylight levels"

      LABEL, "Lighting Controls", STD, LEFT, 20, 58, 1, 0, 0, 345, 12061, 3
      COMBO, 18244, 12048,    0, 1, SPACE, 0, LTG-CTRL-METHOD1, -1, STD, 145,  75, 300, 200, 19, 3,        "System 1 Scenerio:",  LEFT, -115, 5, 0, LEFT, 4, 5, "the type of electric lighting control system at LIGHT-REF-POINT1"
      COMBO, 18245, 12061, 3006, 1, SPACE, 0, LTG-CTRL-METHOD2, -1, STD, 145, 100, 300, 200, 19, 3,        "System 2 Scenerio:",  LEFT, -115, 5, 0, LEFT, 4, 5, "the type of electric lighting control system at LIGHT-REF-POINT2"
      LABEL, "System 1", STD, CENTER, 227, 125, 1, 0, 0, 0, 12061, 3
      LABEL, "System 2", STD, CENTER, 317, 125, 1, 0, 0, 0, 12061, 3
      LABEL, "Continuous Controls", STD, LEFT, 30, 135, 1, 0, 0, 345, 12061, 3
       EDIT, 12056, 12056, 3006, 1, SPACE, 0,   MIN-POWER-FRAC, -1, STD, 200, 155,  23,  55,  3, 3,    "Minimum Power Fraction:",  LEFT, -150, 5, 0, LEFT, 4, 5, "The minimum input power required by a continuous dimming lighting controller"
       EDIT, 18307, 12056, 3006, 1, SPACE, 0,  MIN-POWER-FRAC2, -1, STD, 290, 155,  23,  55,  3, 3,                           "",  LEFT,    0, 5, 0, LEFT, 4, 5, "The minimum input power required by a continuous dimming lighting controller"
       EDIT, 12057, 12057, 3006, 1, SPACE, 0,   MIN-LIGHT-FRAC, -1, STD, 200, 180,  23,  55,  3, 3,    "Minimum Light Fraction:",  LEFT, -150, 5, 0, LEFT, 4, 5, "The minimum light output achieved by a continuous dimming lighting controller"
       EDIT, 18308, 12057, 3006, 1, SPACE, 0,  MIN-LIGHT-FRAC2, -1, STD, 290, 180,  23,  55,  3, 3,                           "",  LEFT,    0, 5, 0, LEFT, 4, 5, "The minimum light output achieved by a continuous dimming lighting controller"
      LABEL, "Equal Stepped Controls", STD, LEFT, 30, 205, 1, 0, 0, 345, 12061, 3
       EDIT, 12058, 12058, 3006, 1, SPACE, 0, LIGHT-CTRL-STEPS, -1, STD, 200, 225,  23,  55,  0, 3,       "Light Control Steps:",  LEFT, -150, 5, 0, LEFT, 4, 5, "The number of steps in a stepped lighting control system (excluding the off state)"
       EDIT, 18309, 12058, 3006, 1, SPACE, 0, LIGHT-CTRL-STEP2, -1, STD, 290, 225,  23,  55,  0, 3,                           "",  LEFT,    0, 5, 0, LEFT, 4, 5, "The number of steps in a stepped lighting control system (excluding the off state)"
       EDIT, 12060, 12060, 3006, 1, SPACE, 0,  LIGHT-CTRL-PROB, -1, STD, 200, 250,  23,  55,  2, 3, "Light Control Probability:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Probability of manually switched lights being switched in response to daylight levels"
       EDIT, 18310, 12060, 3006, 1, SPACE, 0, LIGHT-CTRL-PROB2, -1, STD, 290, 250,  23,  55,  2, 3,                           "",  LEFT,    0, 5, 0, LEFT, 4, 5, "Probability of manually switched lights being switched in response to daylight levels"

; SAC 1/18/06 - mods for T-24 2005
;      LABEL, "Compliance", STD, LEFT, 430,  8, 1, 0, 0, 680, 18215, 1
; AFR 5/18/09 - moved to the lighting tab
;       EDIT, 18215,     0,    0, 1, SPACE, 0,    C-DAYLIT-AREA, -1, STD, 555,  30,  23,  70,  2, 1,               "Daylit Area:",  LEFT, -115, 5, 1, LEFT, 4, 5, ""
; AFR 6/30/09 - removed
;       EDIT, 18216,     0,    0, 1, SPACE, 0,      C-DAYLIT-KW, -1, STD, 555,  30,  23,  70,  2, 1,            "Daylight Power:",  LEFT, -115, 5, 1, LEFT, 4, 5, ""
;      COMBO, 18217,     0,    0, 1, SPACE, 0,  C-DAYLIGHT-CTRL, -1, STD, 510,  55, 100, 133, 19, 1,                "DL Control:",  LEFT,  -70, 5, 0, LEFT, 4, 5, ""


      LABEL, "Discrete Step Controls", STD, LEFT,370, 128, 0, 0, 1, 680, 12061, 3
       SPREAD, 18246, 11692, 0, 1, 0, PowerDOE, 0,  SpaceDiscreteSpread,  0, STD, 370, 150, 130, 310, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""

      LABEL, "Control Reference Points & Settings",     STD,   LEFT,  30, 278, 0, 0, 1, 680, 12049, 3
      LABEL, "Controlled",                    STD, CENTER, 128, 300, 1, 0, 0,   0, 12061, 3
      LABEL, "kW Fraction",                   STD, CENTER, 128, 316, 1, 0, 0,   0, 12061, 3
      LABEL, "Light Set",                     STD, CENTER, 198, 300, 1, 0, 0,   0, 12061, 3
      LABEL, "Point (fc)",                    STD, CENTER, 198, 316, 1, 0, 0,   0, 12061, 3
      LABEL, "Discomfort Glare",              STD, CENTER, 290, 288, 1, 0, 0,   0, 12061, 3
      LABEL, "Max",                           STD, CENTER, 262, 300, 1, 0, 0,   0, 12061, 3
      LABEL, "Value",                         STD, CENTER, 262, 316, 1, 0, 0,   0, 12061, 3
      LABEL, "View",                          STD, CENTER, 322, 300, 1, 0, 0,   0, 12061, 3
      LABEL, "Azimuth",                       STD, CENTER, 322, 316, 1, 0, 0,   0, 12061, 3
      LABEL, "Control System",                STD, CENTER, 408, 300, 1, 0, 0,   0, 12061, 3
      LABEL, "Operation Mode",                STD, CENTER, 408, 316, 1, 0, 0,   0, 12061, 3
      LABEL, "Control Reference Position:",   STD, CENTER, 580, 300, 1, 0, 0,   0, 12061, 3
      LABEL, "X",                             STD, CENTER, 510, 316, 1, 0, 0,   0, 12061, 3
      LABEL, "Y",                             STD, CENTER, 580, 316, 1, 0, 0,   0, 12061, 3
      LABEL, "Z",                             STD, CENTER, 650, 316, 1, 0, 0,   0, 12061, 3

       EDIT, 12049, 12049, 3006, 1, SPACE, 0,   ZONE-FRACTION1, -1, STD, 100, 335,  23,  55,  2, 3,  "System 1:", LEFT,  -70, 5, 0, LEFT, 4, 5, "Fraction of installed lighting kW in the selected space controlled by Lighting System 1"
       EDIT, 12051, 12051, 3006, 1, SPACE, 0, LIGHT-SET-POINT1, -1, STD, 170, 335,  23,  55,  0, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Desired illuminance level for the second Daylite zone in the space is calculated at this point"
       EDIT, 12055, 12055,  762, 1, SPACE, 0,        MAX-GLARE, -1, STD, 240, 335,  23,  45,  0, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Maximum tolerable glare before glare control shading devices are deployed"
       EDIT, 12086, 63035, 3006, 1, SPACE, 0,     VIEW-AZIMUTH, -1, STD, 300, 335,  23,  45,  1, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Direction of the occupant's view (in horizontal plane) in which the daylight glare is calculated for system 1"
      COMBO, 12053, 12053, 3006, 1, SPACE, 0, LIGHT-CTRL-TYPE1, -1, STD, 360, 335,  80, 105, 19, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Lighting controller type for lights lighting system 1"
       EDIT, 13821, 13821, 3006, 1, SPACE, 0, LIGHT-REF-POINT1,  0, STD, 480, 335,  23,  60,  1, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "The desired illuminance level for the first Daylit zone in the space is calculated at this point"
       EDIT, 13822, 13821, 3006, 1, SPACE, 0, LIGHT-REF-POINT1,  1, STD, 550, 335,  23,  60,  1, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "The desired illuminance level for the first Daylit zone in the space is calculated at this point"
       EDIT, 13823, 13821, 3006, 1, SPACE, 0, LIGHT-REF-POINT1,  2, STD, 620, 335,  23,  60,  1, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "The desired illuminance level for the first Daylit zone in the space is calculated at this point"

       EDIT, 12050, 12050, 3006, 1, SPACE, 0,   ZONE-FRACTION2, -1, STD, 100, 360,  23,  55,  2, 3,  "System 2:", LEFT,  -70, 5, 0, LEFT, 4, 5, "Fraction of installed lighting kW in the selected space controlled by Lighting System 2"
       EDIT, 12052, 12052, 3006, 1, SPACE, 0, LIGHT-SET-POINT2, -1, STD, 170, 360,  23,  55,  0, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Desired lighting level at Lighting Ref Point 2 (that Daylighting controls attempt to maintain)"
       EDIT, 18311, 12055,  762, 1, SPACE, 0,       MAX-GLARE2, -1, STD, 240, 360,  23,  45,  0, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Maximum tolerable glare before glare control shading devices are deployed"
       EDIT, 18312, 63035, 3006, 1, SPACE, 0,    VIEW-AZIMUTH2, -1, STD, 300, 360,  23,  45,  1, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Direction of the occupant's view (in horizontal plane) in which the daylight glare is calculated for system 2"
      COMBO, 12054, 12054, 3006, 1, SPACE, 0, LIGHT-CTRL-TYPE2, -1, STD, 360, 360,  80, 105, 19, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Lighting controller type for lights lighting system 2"
       EDIT, 13837, 13837, 3006, 1, SPACE, 0, LIGHT-REF-POINT2,  0, STD, 480, 360,  23,  60,  1, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Desired illuminance level for the second Daylit zone in the space is calculated at this point"
       EDIT, 13838, 13837, 3006, 1, SPACE, 0, LIGHT-REF-POINT2,  1, STD, 550, 360,  23,  60,  1, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Desired illuminance level for the second Daylit zone in the space is calculated at this point"
       EDIT, 13839, 13837, 3006, 1, SPACE, 0, LIGHT-REF-POINT2,  2, STD, 620, 360,  23,  60,  1, 3, "",           LEFT,    0, 5, 0, LEFT, 4, 5, "Desired illuminance level for the second Daylit zone in the space is calculated at this point"
  
    ;******************************************
    ; Space - Contents (Obstructions and Furniture) Page
    ;******************************************
    TABPAGE, 3007, 3007, 1, 3, NOTIMP, " Contents "
      
      LABEL, "Obstructions for Skylight Daylight Calculation", STD,   LEFT,  30,  3,  1, 0, 0, 350, 18264, 3
      LABEL, "Ref Point 1",                                    STD, CENTER, 190, 18,  1, 0, 0,   0, 18264, 3
      LABEL, "Ref Point 2",                                    STD, CENTER, 300, 18,  1, 0, 0,   0, 18264, 3
     COMBO, 18264, 12033, 799, 1, SPACE, 0,   SKY-OBS1-TYPE, -1, STD, 140,  33, 150, 100, 19, 3,"Obstructions:",  LEFT, -100, 5, 0, LEFT, 4, 5, ""
     COMBO, 18265, 12033, 799, 1, SPACE, 0,   SKY-OBS2-TYPE, -1, STD, 250,  33, 150, 100, 19, 3,             "",  LEFT,    0, 5, 0, LEFT, 4, 5, ""
     COMBO, 18266, 12033, 799, 1, SPACE, 0, SKY-OBS1-METHOD, -1, STD, 140,  58, 150, 100, 19, 3, "Factor From:",  LEFT, -100, 5, 0, LEFT, 4, 5, ""
     COMBO, 18267, 12033, 799, 1, SPACE, 0, SKY-OBS2-METHOD, -1, STD, 250,  58, 150, 100, 19, 3,             "",  LEFT,    0, 5, 0, LEFT, 4, 5, ""
      EDIT, 18268, 12034, 799, 1, SPACE, 0, SKY-OBS1-FACTOR, -1, STD, 150,  83,  23,  70,  3, 3,"Factor Value:",  LEFT,  -90, 5, 0, LEFT, 4, 5, ""
      EDIT, 18269, 12034, 799, 1, SPACE, 0, SKY-OBS2-FACTOR, -1, STD, 260,  83,  23,  70,  3, 3,             "",  LEFT,    0, 5, 0, LEFT, 4, 5, ""
      EDIT, 18277, 12034, 799, 1, SPACE, 0,     SKY-OBS1-HT, -1, STD, 150, 108,  23,  70,  2, 3,      "Height:",  LEFT,  -90, 5, 1, LEFT, 4, 5, ""
      EDIT, 18278, 12034, 799, 1, SPACE, 0,     SKY-OBS2-HT, -1, STD, 260, 108,  23,  70,  2, 3,             "",  LEFT,    0, 5, 1, LEFT, 4, 5, ""
      EDIT, 18279, 12034, 799, 1, SPACE, 0,    SKY-OBS1-WID, -1, STD, 150, 133,  23,  70,  2, 3,       "Width:",  LEFT,  -90, 5, 1, LEFT, 4, 5, ""
      EDIT, 18280, 12034, 799, 1, SPACE, 0,    SKY-OBS2-WID, -1, STD, 260, 133,  23,  70,  2, 3,             "",  LEFT,    0, 5, 1, LEFT, 4, 5, ""
      EDIT, 18281, 12034, 799, 1, SPACE, 0,    SKY-OBS1-LEN, -1, STD, 150, 158,  23,  70,  2, 3,      "Length:",  LEFT,  -90, 5, 1, LEFT, 4, 5, ""
      EDIT, 18282, 12034, 799, 1, SPACE, 0,    SKY-OBS2-LEN, -1, STD, 260, 158,  23,  70,  2, 3,             "",  LEFT,    0, 5, 1, LEFT, 4, 5, ""
      EDIT, 18270, 12034, 799, 1, SPACE, 0,   SKY-OBS1-REFL, -1, STD, 150, 183,  23,  70,  3, 3, "Reflectance:",  LEFT,  -90, 5, 0, LEFT, 4, 5, ""
      EDIT, 18271, 12034, 799, 1, SPACE, 0,   SKY-OBS2-REFL, -1, STD, 260, 183,  23,  70,  3, 3,             "",  LEFT,    0, 5, 0, LEFT, 4, 5, ""
     
      LABEL, "Obstructions for Vertical Window Daylight Calculation", STD,   LEFT,  30,213,  1, 0, 0, 350, 18272, 3
      EDIT, 18272, 12034, 799, 1, SPACE, 0,VERT-OBS1-FACTOR, -1, STD, 150, 233,  23,  70,  3, 3,"Factor Value:",  LEFT,  -90, 5, 0, LEFT, 4, 5, ""
      EDIT, 18273, 12034, 799, 1, SPACE, 0,VERT-OBS2-FACTOR, -1, STD, 260, 233,  23,  70,  3, 3,             "",  LEFT,    0, 5, 0, LEFT, 4, 5, ""
     
      LABEL, "Dimensions for Space Coefficient of Utilization for", STD,   LEFT,  30,263,  1, 0, 0, 350, 18274, 3
      LABEL, "Daylighting Obstruction Calculation",                 STD,   LEFT,  30,278,  1, 0, 0,   0, 18274, 3
      EDIT, 18274, 12034, 799, 1, SPACE, 0,   SKY-CU-SPC-HT, -1, STD, 150, 303,  23,  70,  2, 3,      "Height:",  LEFT,  -90, 5, 1, LEFT, 4, 5, ""
      EDIT, 18275, 12034, 799, 1, SPACE, 0,  SKY-CU-SPC-WID, -1, STD, 150, 328,  23,  70,  2, 3,       "Width:",  LEFT,  -90, 5, 1, LEFT, 4, 5, ""
      EDIT, 18276, 12034, 799, 1, SPACE, 0,  SKY-CU-SPC-LEN, -1, STD, 150, 353,  23,  70,  2, 3,       "Depth:",  LEFT,  -90, 5, 1, LEFT, 4, 5, ""

      LABEL, "Use Custom or Standard Weighting Factors", STD, LEFT, 380, 3, 1, 0, 0, 665, 12033, 3
      LABEL, "(Floor Weight > 0 uses standard values)",  STD, LEFT, 380,18, 1, 0, 0,   0, 12033, 3
      EDIT, 12031, 12031, 799, 1, SPACE, 0,     FLOOR-WEIGHT, -1, STD, 545,  35,  21,  70,  2, 3,           "Floor Weight:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Total weight of interior furnishings and surrounding surfaces of a space per unit floor area"
    
      LABEL, "Internal Mass for Custom Weighting Factor Calc", STD, LEFT, 380, 72, 1, 0, 0, 665, 12033, 3
      LABEL, "(Used only if Floor Weight = 0)",                STD, LEFT, 380, 88, 1, 0, 0,   0, 12033, 3
      LABEL, "Furniture and Contents Coverage and Mass",       STD, LEFT, 380,118, 1, 0, 0,   0, 12033, 3
     COMBO, 12033, 12033, 799, 1, SPACE, 0,   FURNITURE-TYPE, -1, STD, 545, 135,  60, 100, 19, 3,         "Furniture Type:",  LEFT, -145, 5, 0, LEFT, 4, 5, "Furniture type (Light is approx 40 lb/cubic ft; Heavy is approx 80 lb/cubic ft)"
      EDIT, 12034, 12034, 799, 1, SPACE, 0,    FURN-FRACTION, -1, STD, 545, 160,  23,  70,  2, 3, "Fraction of Floor Area:",  LEFT, -145, 5, 0, LEFT, 4, 5, "The fraction of floor area covered by furniture"
      EDIT, 12035, 12035, 799, 1, SPACE, 0,      FURN-WEIGHT, -1, STD, 545, 185,  23,  70,  2, 3,                 "Weight:",  LEFT, -145, 5, 1, LEFT, 4, 5, "The weight of the furniture per unit floor area"
      LABEL, "Calculated Custom Weighting Factor",             STD, LEFT, 380,228, 1, 0, 0,   0, 12033, 3
     COMBO, 12032, 12032, 799, 0, SPACE, 0, WEIGHTING-FACTOR, -1, STD, 525, 250, 220, 140, 19, 3,       "Weighting Factor:",  LEFT, -125, 5, 0, LEFT, 4, 5, "Name of user-calculated weighting factors to be stored in or recalled from the library"

;   ;******************************************
;   ; Bldg - Zone - Lighting System Dialog
;   ;******************************************
;  MODTABDLG, 3060, 32084, 1, 100, 100, 355, 610, 0, "Lighting Data for Space:   ", SPACE, 0, NAME, -1, 32, 0, "", NOTIMP, 0, NOTIMP, 0
      
    ;*****************************************
    ; Space - Lighting System/Power Page
    ;*****************************************
;    TABPAGE, 3064, 3064, 1, 3, NOTIMP, " Lighting System/Power "
    TABPAGE, 3064, 3064, 1, 3, NOTIMP, " Lighting "
  
      COMBO, 19041, 19041, 32084, 1, SPACE, 0, LTG-SPEC-METHOD, -1, STD, 200, 10, 80, 150, 19, 3, "Lighting Data Input Method:", LEFT, -170, 5, 0, LEFT, 4, 5, "Power Defn=simplified;Luminaire Count=Lighting Systems;Illuminance=light level desired"

; SAC 3/27/09 - removed individual (single element) controls providing access to keywords converted into arrays and integrated into lighting spreadsheets
;      LABEL, "This Space", STD, CENTER, 215, 183, 1, 0, 0, 0, 13573, 3
;      LABEL, "Adj. Space", STD, CENTER, 290, 183, 1, 0, 0, 0, 13574, 3
;      LABEL, "Return Air", STD, CENTER, 365, 183, 1, 0, 0, 0, 13575, 3
;
;       EDIT, 13573, 13573,   772, 1, SPACE, 0,   LIGHT-TO-SPACE, -1, STD, 190, 200,  23,  50,  2, 3,       "Fraction of Light Heat:", RIGHT,  -15, 5, 0, LEFT, 4, 5, "Fraction of the lighting power consumption that appears in the space as heat"  
;       EDIT, 13574, 13574,   772, 1, SPACE, 0,   LIGHT-TO-OTHER, -1, STD, 265, 200,  23,  50,  2, 3,                              "", RIGHT,    0, 5, 0, LEFT, 4, 5, "Fraction of the lighting power consumption that appears in an adjacent space as heat"  
;       EDIT, 13575, 13575,   772, 1, SPACE, 0,  LIGHT-TO-RETURN, -1, STD, 340, 200,  23,  50,  2, 3,                              "", RIGHT,    0, 5, 0, LEFT, 4, 5, "Fraction of lighting power consumption that appears in the return air stream space as heat"
;
;       EDIT, 13576, 13576,   771, 1, SPACE, 0,   LIGHT-RAD-FRAC,  0, STD, 190, 225,  23,  50,  2, 3,             "Radiant Fraction:", RIGHT,  -15, 5, 0, LEFT, 4, 5, "The fraction of heat (from lights) in the space that is radiative (the remainder is convective)"       
;       EDIT, 13577, 13577,   771, 1, SPACE, 0,   LIGHT-RAD-FRAC,  1, STD, 265, 225,  23,  50,  2, 3,                              "", RIGHT,    0, 5, 0, LEFT, 4, 5, "The fraction of heat (from lights) in the space that is radiative (the remainder is convective)"
;
;      COMBO, 13578, 13578,   772, 1, SPACE, 0,    LIGHT-HEAT-TO, -1, STD, 220, 250, 220, 170, 19, 3, "Adj. Space Light Ht. Goes To:",  LEFT, -180, 5, 0, LEFT, 4, 5, "An adjacent space that receives the Fraction of Light Heat to Adjacent Space"    

; AFR 5/12/09 - moved per Luke email 5/11/09.
      LABEL, "Task Lighting", STD, LEFT, 750, 10, 1, 0, 0, 995, 13581, 3
      COMBO, 13581, 13581, 32084, 1, SPACE, 0,   TASK-LIGHT-SCH, -1, STD, 815, 35, 220, 185, 19, 3,                     "Schedule:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "Schedule of operation for all the task lights in the space (schedule type should be Fraction)"
       EDIT, 13579, 13579, 32084, 1, SPACE, 0,   TASK-LT-W/AREA, -1, STD, 845, 60,  23,  50,  2, 3,                "Power Density:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Maximum energy consumption of task lighting, per square feet of space floor area"     
       EDIT, 13580, 13580, 32084, 1, SPACE, 0, TASK-LIGHTING-KW, -1, STD, 845, 85,  23,  50,  2, 3,                        "Power:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Maximum energy consumption of task lighting"

       EDIT, 14598,  1517, 32084, 1, SPACE, 0, WORKPLANE-HEIGHT, -1, STD, 845, 125,  23,  50,  2, 3, "Workplane Height:",        LEFT, -155, 5, 1, LEFT, 4, 5, "Distance from the floor to the workplane; DOE-2 calculates the Illuminance at this height"

      LABEL, "Power Summary",      STD,  LEFT,         760, 205,  1, 0, 0, 995, 0, 3
     STATIC, 1, SPACE,  0, UNITS,            29, 0, 2, 940, 221, -1, STD, RIGHT, "", "", 0, 3
     STATIC, 1, SPACE,  0, UNITS,            28, 0, 2, 995, 221, -1, STD, RIGHT, "", "", 0, 3
      LABEL, "Overhead Lighting:", STD, RIGHT,         885, 239,  1, 0, 0,   0, 0, 3
      LABEL, "    Task Lighting:", STD, RIGHT,         885, 257,  1, 0, 0,   0, 0, 3
      LABEL, "  Misc. Equipment:", STD, RIGHT,         885, 275,  1, 0, 0,   0, 0, 3
     STATIC, 1, SPACE,  0, *DISP-LIGHT-W/AR, -1, 0, 3, 940, 239, -1, STD, RIGHT, "", "", 0, 3
     STATIC, 1, SPACE,  0, *DISP-TASK-W/AR , -1, 0, 3, 940, 257, -1, STD, RIGHT, "", "", 0, 3
     STATIC, 1, SPACE,  0, *DISP-EQUIP-W/AR, -1, 0, 3, 940, 275, -1, STD, RIGHT, "", "", 0, 3
     STATIC, 1, SPACE,  0, *DISP-LIGHT-KW,   -1, 0, 2, 995, 239, -1, STD, RIGHT, "", "", 0, 3
     STATIC, 1, SPACE,  0, *DISP-TASK-KW,    -1, 0, 2, 995, 257, -1, STD, RIGHT, "", "", 0, 3
     STATIC, 1, SPACE,  0, *DISP-EQUIP-KW,   -1, 0, 2, 995, 275, -1, STD, RIGHT, "", "", 0, 3
;      LABEL, "Task Lighting", STD, LEFT, 30, 263, 1, 0, 0, 290, 13581, 3
;      COMBO, 13581, 13581, 32084, 1, SPACE, 0,   TASK-LIGHT-SCH, -1, STD, 105, 285, 220, 185, 19, 3,                     "Schedule:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "Schedule of operation for all the task lights in the space (schedule type should be Fraction)"
;       EDIT, 13579, 13579, 32084, 1, SPACE, 0,   TASK-LT-W/AREA, -1, STD, 135, 310,  23,  50,  2, 3,                "Power Density:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Maximum energy consumption of task lighting, per square feet of space floor area"     
;       EDIT, 13580, 13580, 32084, 1, SPACE, 0, TASK-LIGHTING-KW, -1, STD, 135, 335,  23,  50,  2, 3,                        "Power:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Maximum energy consumption of task lighting"
;
;       EDIT, 14598,  1517, 32084, 1, SPACE, 0, WORKPLANE-HEIGHT, -1, STD, 590, 235,  23,  50,  2, 3, "Workplane Height:",        LEFT, -155, 5, 1, LEFT, 4, 5, "Distance from the floor to the workplane; DOE-2 calculates the Illuminance at this height"
;
;      LABEL, "Power Summary",      STD,  LEFT,         435, 295,  1, 0, 0, 675, 0, 3
;     STATIC, 1, SPACE,  0, UNITS,            29, 0, 2, 620, 311, -1, STD, RIGHT, "", "", 0, 3
;     STATIC, 1, SPACE,  0, UNITS,            28, 0, 2, 675, 311, -1, STD, RIGHT, "", "", 0, 3
;      LABEL, "Overhead Lighting:", STD, RIGHT,         565, 329,  1, 0, 0,   0, 0, 3
;      LABEL, "    Task Lighting:", STD, RIGHT,         565, 347,  1, 0, 0,   0, 0, 3
;      LABEL, "  Misc. Equipment:", STD, RIGHT,         565, 365,  1, 0, 0,   0, 0, 3
;     STATIC, 1, SPACE,  0, *DISP-LIGHT-W/AR, -1, 0, 3, 620, 329, -1, STD, RIGHT, "", "", 0, 3
;     STATIC, 1, SPACE,  0, *DISP-TASK-W/AR , -1, 0, 3, 620, 347, -1, STD, RIGHT, "", "", 0, 3
;     STATIC, 1, SPACE,  0, *DISP-EQUIP-W/AR, -1, 0, 3, 620, 365, -1, STD, RIGHT, "", "", 0, 3
;     STATIC, 1, SPACE,  0, *DISP-LIGHT-KW,   -1, 0, 2, 675, 329, -1, STD, RIGHT, "", "", 0, 3
;     STATIC, 1, SPACE,  0, *DISP-TASK-KW,    -1, 0, 2, 675, 347, -1, STD, RIGHT, "", "", 0, 3
;     STATIC, 1, SPACE,  0, *DISP-EQUIP-KW,   -1, 0, 2, 675, 365, -1, STD, RIGHT, "", "", 0, 3

     ;*****  Lighting Power Mode  *****
     CASE,  SPACE,  0, LTG-SPEC-METHOD,  -1, =, 1, 0
        SPREAD, 11524, 0, 0, 1, 0, PowerDOE, 0, SpaceLightPow, 0, STD, 40, 45, 180, 625, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     ENDCASE

     CASE, ELSE
; AFR 5/12/09 - moved per Luke email.     
        EDIT,  13582, 13582,     0, 1, SPACE, 0,    LUM-SPACE-DIV, -1, STD, 845, 150,  23,  50,  1, 3, "Luminaire Space Divider:", LEFT, -155, 5, 1, LEFT, 4, 5, "The space is divided into this number identical rooms for the lighting calculations"
;        EDIT,  13582, 13582,     0, 1, SPACE, 0,    LUM-SPACE-DIV, -1, STD, 590, 260,  23,  50,  1, 3, "Luminaire Space Divider:", LEFT, -155, 5, 1, LEFT, 4, 5, "The space is divided into this number identical rooms for the lighting calculations"

        SPREAD, 11522, 11522, 0, 1, 0, PowerDOE, 0,   SpaceLightSys, 0, STD, 40, 45, 180, 625, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
; The following two spreadsheets are identical, so I replaced the CASE w/ a single SPREAD (above)
;        ;*****  Lighting System Mode  *****
;        CASE,  SPACE,  0, LTG-SPEC-METHOD,  -1, =, 1, 1
;           SPREAD, 11522, 11522, 0, 1, 0, PowerDOE, 0,   SpaceLightSys, 0, STD, 40, 55, 150, 625, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
;        ENDCASE
;
;        ;*****  Lighting Illuminance Mode  *****
;        CASE,  SPACE,  0, LTG-SPEC-METHOD,  -1, =, 1, 2
;           SPREAD, 11545, 11545, 0, 1, 0, PowerDOE, 0, SpaceLightIllum, 0, STD, 40, 55, 150, 625, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
;        ENDCASE

        CASE,  SPACE,  0, LTG-SPEC-METHOD,  -1, =, 1, 1
           BUTTON, 10249, 10249, 0, 1, 92, 3167, STD, 495,  15, 23, 170, 3, "Lighting System Data...", ""
        ENDCASE

     ENDCASE

; AFR 5/12/09 - added  -  AFR 7/27/09 - rework.
      LABEL, "Compliance Data", STD, LEFT, 30, 223, 1, 0, 0, 725, 0, 7
       EDIT, 13578, 13578, 0, 1, SPACE, 0, C-DAYLIT-AREA,        -1, STD, 260, 240,  23,  80,  0, 7, "Non-Exempt Required Daylit Area:",         LEFT,  -206, 5, 1, LEFT, 4, 5, "Area Subject to 143C"
       EDIT, 13587, 13587, 0, 1, SPACE, 0, C-XMT-DAYLT-AREA,     -1, STD, 260, 265,  23,  80,  0, 7, "Exempt Required Daylit Area:",             LEFT,  -180, 5, 1, LEFT, 4, 5, "Exempt Required Daylit Area"
       EDIT, 13585, 13585, 0, 1, SPACE, 0, C-CUSTOM-LTG-KW1,     -1, STD, 630, 240,  23,  80,  2, 7, "General Tailored Lighting Allowance:",     LEFT,  -213, 5, 1, LEFT, 4, 5, ""
       EDIT, 13586, 13586, 0, 1, SPACE, 0, C-CUSTOM-LTG-KW2,     -1, STD, 630, 265,  23,  80,  2, 7, "Additional Tailored Lighting Allowance:",  LEFT,  -225, 5, 1, LEFT, 4, 5, ""
      COMBO, 13588, 13588, 0, 1, SPACE, 0, C-DAYLIT-XMTN,        -1, STD, 260, 290, 220, 185, 19, 7, "Exemption(s):"                          ,  LEFT,   -90, 5, 0, LEFT, 4, 5, "Reason for exemption"
       
     SPREAD, 11521, 11521, 0, 1, 0, PowerDOE, 0, SpaceLightComp,  0, STD,  40, 330, 160, 730, 19, 7, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""

; AFR 5/14/09 - removed.
;; SAC 11/25/00 - Compliance keywords
;    ;******************************************
;    ; Space - Compliance Page
;    ;******************************************
;    TABPAGE, 3233, 3233, 1, 1, NOTIMP, " Compliance "
;
;      LABEL, "Lighting Loads by Occupancy Type",                         STD, LEFT, 20,   6, 1, 0, 0, 680, 0, 1
;     SPREAD, 15593, 15593, 0, 1, 0, PowerDOE, 0,  SpaceCompLtgSpread,      0, STD,  30,  24,  85, 650, 19, 1, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
;
;      LABEL, "Tailored Vent & Lighting and Control Credits",             STD, LEFT, 20, 119, 1, 0, 0, 680, 0, 1
;     SPREAD, 15594, 15594, 0, 1, 0, PowerDOE, 0,  SpaceCompTailoredSpread, 0, STD,  30, 137, 100, 650, 19, 1, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
;
;; SAC 7/25/06 - removed per KJM e-mail of 6/27/06
;;      LABEL, "Process Energy Use",                                       STD, LEFT, 20, 247, 1, 0, 0, 680, 0, 1
;;     SPREAD, 15595, 15595, 0, 1, 0, PowerDOE, 0,  SpaceCompSourceSpread,   0, STD,  30, 265,  85, 650, 19, 1, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
;
;;      LABEL, "Number of LTG-1 Report Records", STD, LEFT, 30, 330, 1, 0, 0, 525, 0, 1
;;       EDIT, 15591, 15591, 0, 1,  SPACE, 0,   C-NUM-MCTRL-RCDS, -1, STD, 240, 350,  23,  60,  0, 1,  "Mandatory Automatic Controls:", RIGHT,   -8, 5, 1, LEFT, 4, 5, ""
;;       EDIT, 15592, 15592, 0, 1,  SPACE, 0,   C-NUM-CCTRL-RCDS, -1, STD, 465, 350,  23,  60,  0, 1,           "Controls for Credit:", RIGHT,   -8, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Number of LTG-1 Report Records:", STD, LEFT, 20, 362, 1, 0, 0, 0, 0, 1
;       EDIT, 15591, 15591, 0, 1,  SPACE, 0,   C-NUM-MCTRL-RCDS, -1, STD, 430, 357,  23,  50,  0, 1,  "Mandatory Automatic Controls:", RIGHT,   -7, 5, 1, LEFT, 4, 5, "The number of blank lines to print for listing mandatory controls for this space"
;       EDIT, 15592, 15592, 0, 1,  SPACE, 0,   C-NUM-CCTRL-RCDS, -1, STD, 630, 357,  23,  50,  0, 1,           "Controls for Credit:", RIGHT,   -7, 5, 1, LEFT, 4, 5, "The number of blank lines to print for listing controls for credit for this space"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Exterior Wall - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

 MODTABDLG, 3008, 3008, 1, 30, 30, 480, 440, 0, EXTERIOR-WALL, "Exterior Surface Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 12402, 3008, 0, 1, EXTERIOR-WALL, 0, NAME,  0, STD, 175,  15, 400, 250, 19, 3, "Currently Active Surface:",  LEFT, -155, 5, 0, LEFT, 4, 5, "List of all exterior surfaces defined in project; also allows library retrieval and creation"

    ;******************************************
    ; Exterior Wall - Basic Specs Page
    ;******************************************
;    DATAWIN, 2004, 2004, 1, BLDG_FLR_XW, 135, -1
    TABPAGE, 3211, 2004, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 12095, 12095,     0, 1,  EXTERIOR-WALL, 0,             NAME, -1, STD, 125,  10,  23, 250, 32, 3,  "Surface Name:",  LEFT, -95, 5, 0, LEFT, 4, 5, "Name of exterior surface; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 15621, 15621,     0, 1,  EXTERIOR-WALL, 0,           PARENT, -1, STD, 125,  65, 220, 250, 19, 3,  "Parent Space:",  LEFT, -95, 5, 0, LEFT, 4, 5, ""
      COMBO, 19180,  2502,     0, 1,  EXTERIOR-WALL, 0,     CONSTRUCTION, -1, STD, 125,  90, 220, 250, 19, 3,  "Construction:",  LEFT, -95, 5, 0, LEFT, 4, 5, "The construction (Layers) of the surface"
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
; NAVEDIT, 12009, 12091,   0, 1, 3135, EXTERIOR-WALL, 0, CONSTRUCTION, -1, CONSTRUCTION, 0, U-VALUE, -1, STD, 330,  32,  21,  45,  3, 3,   "U-Val:",  LEFT, 275,  34, 1, LEFT, 380,  34, "Overall thermal conductance of this surface (less exterior film resistance, dbl click to edit)"
; NAVEDIT, 12010, 19017,   0, 1, 3135, EXTERIOR-WALL, 0, CONSTRUCTION, -1, CONSTRUCTION, 0,  LAYERS, -1, STD, 330,  57,  21, 110,  0, 3,  "Layers:",  LEFT, 275,  59, 0, LEFT, 485,  59, "Name of the construction of this wall (alternative to U-Value, dbl click to edit)"

       EDIT, 12001, 12001,   769, 1,  EXTERIOR-WALL, 0,       MULTIPLIER, -1, STD, 125, 115,  23,  45,  0, 3,    "Multiplier:",  LEFT, -95, 5, 0, LEFT, 4, 5, ""

; AFR 6/24/09 - changed compliance flag from 1 to 7 for non-LEED
; SAC 8/30/01 - Compliance keyword
   CHECKBOX, 17500,     0,     0, 1,  EXTERIOR-WALL, 0,      C-COOL-ROOF, -1, STD, 190, 118,  17, 185,     7,      "Cool Roof (compliance)", RIGHT,           "Identifies this exterior wall as a 'cool' (or low-albedo) roof"
; AFR 6/24/09 - changed compliance flag from 1 to 7 for non-LEED
; SAC 10/23/00 - Compliance keyword
   CHECKBOX, 15460,     0,     0, 1,  EXTERIOR-WALL, 0,  C-DEMISING-WALL, -1, STD, 190, 140,  17, 185,     7,  "Demising Wall (compliance)", RIGHT,           "Check if this exterior wall is a demising wall with another space"
; SAC 10/4/04 - Compliance keyword
   CHECKBOX, 17873,     0,     0, 1,  EXTERIOR-WALL, 0,  C-SKYLIGHT-ROOF, -1, STD, 190, 162,  17, 185,     1,  "Skylight Roof (compliance)", RIGHT,           "Check if this surface is a roof with skylights and no tangible heat transfer (U-value < 0.0011)"
; AFR 6/24/09 - changed compliance flag from 1 to 7 for non-LEED
; SAC 12/27/05 - Compliance keyword
; SAC 1/6/10 - removed keywords no longer referenced by T24-08 ruleset (C-METALIC-FINISH)
;   CHECKBOX, 17874,     0,     0, 1,  EXTERIOR-WALL, 0, C-METALIC-FINISH, -1, STD, 190, 184,  17, 185,     7, "Metalic Finish (compliance)", RIGHT,           ""

      LABEL, "Location & Geometry", STD, LEFT, 30, 213, 0, 0, 1, 375, 0, 3
      COMBO, 19015, 19015,   755, 1,  EXTERIOR-WALL, 0,         LOCATION, -1, STD, 110, 235, 220, 265, 19, 3,      "Location:",  LEFT, -60, 5, 0, LEFT, 4, 5, "Positions this surface in the space (applies only if space is defined with Shape or Polygon)"
      COMBO, 19061,   694, 31030, 1,  EXTERIOR-WALL, 0,          POLYGON, -1, STD, 110, 260, 220, 265, 19, 3,       "Polygon:",  LEFT, -60, 5, 0, LEFT, 4, 5, "Name of the Polygon that defines the surface's shape"

       EDIT, 19008, 19008,   755, 1,  EXTERIOR-WALL, 0,                X, -1, STD, 110, 285,  23,  70,  2, 3,             "X:",  LEFT, -60, 5, 1, LEFT, 4, 5, "X coordinate for the surface origin (relative to this Space coordinate system)"
       EDIT, 19009, 19009,   755, 1,  EXTERIOR-WALL, 0,                Y, -1, STD, 110, 310,  23,  70,  2, 3,             "Y:",  LEFT, -60, 5, 1, LEFT, 4, 5, "Y coordinate for the surface origin (relative to this Space coordinate system)"
       EDIT, 19010, 19010,   755, 1,  EXTERIOR-WALL, 0,                Z, -1, STD, 110, 335,  23,  70,  2, 3,             "Z:",  LEFT, -60, 5, 1, LEFT, 4, 5, "Z coordinate for the surface origin (relative to this Space coordinate system)"
       EDIT, 19011, 19011,   755, 1,  EXTERIOR-WALL, 0,          AZIMUTH, -1, STD, 110, 360,  23,  70,  2, 3,       "Azimuth:",  LEFT, -60, 5, 1, LEFT, 4, 5, "Azimuth of surface outward normal relative to Space Y-axis (positive = clockwise rotation)"

       EDIT, 19013, 19013,     0, 1,  EXTERIOR-WALL, 0,           HEIGHT, -1, STD, 285, 285,  23,  74,  2, 3,        "Height:",  LEFT, -50, 5, 1, LEFT, 4, 5, "Dimension of the surface parallel to the Surface Y-axis"
       EDIT, 19014, 19014,     0, 1,  EXTERIOR-WALL, 0,            WIDTH, -1, STD, 285, 310,  23,  74,  2, 3,         "Width:",  LEFT, -50, 5, 1, LEFT, 4, 5, "Width of the surface (measured parallel to the Surface x-axis)."
       EDIT, 19012, 19012,     0, 1,  EXTERIOR-WALL, 0,             TILT, -1, STD, 285, 335,  23,  74,  2, 3,          "Tilt:",  LEFT, -50, 5, 1, LEFT, 4, 5, ""
 
      CASE, EXTERIOR-WALL, 0, LOCATION, -1, =, 1, 1
         LABEL,  "Roof", STD, LEFT, 140, 38, 1, 0, 0, 0, 0, 3
      ENDCASE
      CASE, EXTERIOR-WALL, 0, LOCATION, -1, =, 1, 2
         LABEL, "Floor", STD, LEFT, 140, 38, 1, 0, 0, 0, 0, 3
      ENDCASE
      CASE, ELSE
         STATIC, 1, EXTERIOR-WALL,  0, DEG-FROM-NORTH, -1, 0, 0, 140, 38, -1, STD, LEFT, "Wall Facing ", "° (clockwise from north)", 0, 3
;         LABEL,  "Exterior Wall Name:", STD, RIGHT, 142, 15, 1, 0, 0, 0, 0, 3
;         LABEL, "Faces", STD, LEFT,  450,  7,  1, 0, 0, 3
;         LABEL, "(° clockwise from north):", SMALL, LEFT,  487,  7,  1, 0, 0, 3
;         STATIC, 1, EXTERIOR-WALL,  0, DEG-FROM-NORTH, -1, 0, 0, 630,  7, -1, STD, RIGHT, "", "", 0, 3
      ENDCASE

    ;****************************************************************
    ; Exterior Wall - Daylighting / Shading / Other Page
    ;****************************************************************
;    TABPAGE, 3009, 3006, 1, 3, "Daylighting"
;    TABPAGE, 3010, 3010, 1, 3, "Shading & View"
;    TABPAGE, 3011, 3011, 1, 3, "Other"
    TABPAGE, 3009, 3006, 1, 3, NOTIMP, " Daylighting  -  Shading  -  Other "
 
      LABEL, "Daylighting",    STD, LEFT, 60,  5, 0, 0, 1, 330, 12084, 3
       EDIT, 12084, 12084, 3006, 1, EXTERIOR-WALL, 0,  INSIDE-VIS-REFL, -1, STD, 260,  30, 23, 70,  3, 3,  "Inside Visible Reflectance:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Fraction of the incident visible light reflected by the interior finish of this surface"
 
      LABEL, "Shading & View", STD, LEFT, 60,  60, 0, 0, 1, 330, 12085, 3
       EDIT, 12085, 12085, 3010, 1, EXTERIOR-WALL, 0,  GND-REFLECTANCE, -1, STD, 260, 85, 23, 70,  3, 3,          "Ground Reflectance:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Fraction of solar radiation ('seen' by this exterior surface) that is reflected by the ground plane"
       EDIT, 12088, 12088, 3010, 1, EXTERIOR-WALL, 0, SHADING-DIVISION, -1, STD, 260, 110, 23, 70,  0, 3, "Number of Shading Divisions:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Number of 'vertical' segmentations used in shading calculations for this exterior surface"
      COMBO, 12090, 12090,  777, 1, EXTERIOR-WALL, 0,  SHADING-SURFACE, -1, STD, 260, 135, 80, 70, 19, 3,             "Shading Surface:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Yes causes this exterior surface to also act as a Building Shade."
                                                                   
      LABEL, "Other",          STD, LEFT, 60, 165, 0, 0, 1, 330, 12080, 3
       EDIT, 12080, 12080, 3011, 1, EXTERIOR-WALL, 0,         INF-COEF, -1, STD, 260, 190, 23, 70,  1, 3,    "Infiltration Coefficient:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Infiltration flow coefficient for this exterior surface (used with the infiltration Crack Method)"
       EDIT, 12081, 12081, 3011, 1, EXTERIOR-WALL, 0,    OUTSIDE-EMISS, -1, STD, 260, 215, 23, 70,  3, 3,          "Outside Emissivity:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Infrared (IR) emissivity of the exterior finish of this surface"
       EDIT, 12082, 12082,  753, 1, EXTERIOR-WALL, 0,   INSIDE-SOL-ABS, -1, STD, 260, 240, 23, 70,  3, 3,    "Inside Solar Absorptance:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Fraction of incident total solar radiation absorbed at the interior finish of this surface"
       EDIT, 12083, 12083, 3011, 1, EXTERIOR-WALL, 0,   SOLAR-FRACTION, -1, STD, 260, 265, 23, 70,  3, 3,       "Inside Solar Fraction:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Fraction of solar radiation entering this space that is incident on the interior of this surface"
       EDIT, 19348, 19348,    0, 1, EXTERIOR-WALL, 0,     INSIDE-EMISS, -1, STD, 260, 290, 23, 70,  3, 3,           "Inside Emissivity:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Emissivity of the interior surface: must be consistent with construction LAYERS Inside Film Resistance"
       EDIT, 19349, 19349,    0, 1, EXTERIOR-WALL, 0,     INSIDE-RCONV, -1, STD, 260, 315, 23, 70,  3, 3, "Inside Convective Resistance:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Convective resistance of the interior surface: must be consistent with construction LAYERS Inside Film Resistance"
      LABEL, "Note: If inside emissivity and convective resistance are entered here,",    STD, LEFT, 15, 343, 0, 0, 1, 330, 19348, 3
      LABEL, "the values must be consistent with the inside film resistance entered",     STD, LEFT, 30, 360, 0, 0, 1, 330, 19348, 3
      LABEL, "for the LAYERS command for the associated construction.",                   STD, LEFT, 30, 377, 0, 0, 1, 330, 19348, 3



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Interior Wall - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

 MODTABDLG, 3149, 3149, 1, 30, 30, 460, 440, 0, INTERIOR-WALL, "Interior Surface Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 12409, 3149, 0, 1, INTERIOR-WALL, 0, NAME,  0, STD, 175,  15, 400, 250, 19, 3, "Currently Active Surface:",  LEFT, -155, 5, 0, LEFT, 4, 5, "List of all interior surfaces defined in project; also allows library retrieval and creation"

    ;******************************************
    ; Interior Wall - Basic Specs Page
    ;******************************************
;    DATAWIN, 2010, 2010, 1, BLDG_FLR_IW, 135, -1
    TABPAGE, 3212, 2010, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 12140, 12140,     0, 1,  INTERIOR-WALL, 0,             NAME, -1, STD, 125,  10,  23, 250, 32, 3,  "Surface Name:",  LEFT, -95, 5, 0, LEFT, 4, 5, "Name of interior surface; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 15622, 15622,     0, 1,  INTERIOR-WALL, 0,           PARENT, -1, STD, 125,  65, 220, 250, 19, 3,  "Parent Space:",  LEFT, -95, 5, 0, LEFT, 4, 5, ""
      COMBO, 12522, 12522,     0, 1,  INTERIOR-WALL, 0,     CONSTRUCTION, -1, STD, 125,  90, 220, 250, 19, 3,  "Construction:",  LEFT, -95, 5, 0, LEFT, 4, 5, "The construction (Layers) of the surface"
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
; NAVEDIT, 12167, 12091,     0, 1, 3135, INTERIOR-WALL, 0,  CONSTRUCTION, -1, CONSTRUCTION, 0, U-VALUE, -1, STD, 330,  32,  21,  45,  3, 3, "U-Val:",  LEFT, 275,  34, 1, LEFT, 380,  34, "Overall thermal conductance of this construction (less exterior film resistance)"

      COMBO, 12165, 12165,     0, 1,  INTERIOR-WALL, 0,    INT-WALL-TYPE, -1, STD, 125, 115, 110, 250, 19, 3,  "Surface Type:",  LEFT, -95, 5, 0, LEFT, 4, 5, ""

; AFR 6/24/09 - don't show for LEED
; SAC 10/23/00 - Compliance keyword
   CHECKBOX, 15480,     0,     0, 1, INTERIOR-WALL,  0,  C-DEMISING-WALL, -1, STD, 126, 145,  17, 185,     7,  "Demising Wall (compliance)", RIGHT,           "Check if this interior wall is a demising wall with another space"

      LABEL, "Location & Geometry", STD, LEFT, 30, 178, 0, 0, 1, 375, 0, 3
      COMBO, 12488, 63044,   771, 1,  INTERIOR-WALL, 0,          NEXT-TO, -1, STD, 110, 200, 220, 265, 19, 3,       "Next To:",  LEFT, -60, 5, 0, LEFT, 4, 5, "Name of space on other side of wall (for heat transfer)"
      COMBO, 19070, 19070,   755, 1,  INTERIOR-WALL, 0,         LOCATION, -1, STD, 110, 225, 220, 265, 19, 3,      "Location:",  LEFT, -60, 5, 0, LEFT, 4, 5, "Positions this surface in the space (applies only if space is defined with Shape or Polygon)"
      COMBO, 19062,   694, 31030, 1,  INTERIOR-WALL, 0,          POLYGON, -1, STD, 110, 250, 220, 265, 19, 3,       "Polygon:",  LEFT, -60, 5, 0, LEFT, 4, 5, "Name of the Polygon that defines the surface's shape"

       EDIT, 19065, 19065,   755, 1,  INTERIOR-WALL, 0,                X, -1, STD, 110, 275,  23,  70,  2, 3,             "X:",  LEFT, -60, 5, 1, LEFT, 4, 5, "X coordinate for the surface origin (relative to this Space coordinate system)"
       EDIT, 19066, 19066,   755, 1,  INTERIOR-WALL, 0,                Y, -1, STD, 110, 300,  23,  70,  2, 3,             "Y:",  LEFT, -60, 5, 1, LEFT, 4, 5, "Y coordinate for the surface origin (relative to this Space coordinate system)"
       EDIT, 19067, 19067,   755, 1,  INTERIOR-WALL, 0,                Z, -1, STD, 110, 325,  23,  70,  2, 3,             "Z:",  LEFT, -60, 5, 1, LEFT, 4, 5, "Z coordinate for the surface origin (relative to this Space coordinate system)"
       EDIT, 19068, 19068,   755, 1,  INTERIOR-WALL, 0,          AZIMUTH, -1, STD, 110, 350,  23,  70,  2, 3,       "Azimuth:",  LEFT, -60, 5, 1, LEFT, 4, 5, "Azimuth of surface outward normal relative to Space Y-axis (positive = clockwise rotation)"

       EDIT, 12166, 12166,     0, 1,  INTERIOR-WALL, 0,             AREA, -1, STD, 285, 275,  23,  74,  2, 3,          "Area:",  LEFT, -50, 5, 1, LEFT, 4, 5, "Area of this interior surface (an alternative to entering Height and Width)"
       EDIT, 19071, 19071,     0, 1,  INTERIOR-WALL, 0,           HEIGHT, -1, STD, 285, 300,  23,  74,  2, 3,        "Height:",  LEFT, -50, 5, 1, LEFT, 4, 5, "Dimension of the surface parallel to the Surface Y-axis"
       EDIT, 19072, 19072,     0, 1,  INTERIOR-WALL, 0,            WIDTH, -1, STD, 285, 325,  23,  74,  2, 3,         "Width:",  LEFT, -50, 5, 1, LEFT, 4, 5, "Width of the surface (measured parallel to the Surface x-axis)."
       EDIT, 19069, 19069,   755, 1,  INTERIOR-WALL, 0,             TILT, -1, STD, 285, 350,  23,  74,  2, 3,          "Tilt:",  LEFT, -50, 5, 1, LEFT, 4, 5, ""

      CASE, INTERIOR-WALL, 0, LOCATION, -1, =, 1, 1
         LABEL, "Ceiling", STD, LEFT, 140, 38, 1, 0, 0, 0, 0, 3
      ENDCASE
      CASE, INTERIOR-WALL, 0, LOCATION, -1, =, 1, 2
         LABEL,   "Floor", STD, LEFT, 140, 38, 1, 0, 0, 0, 0, 3
      ENDCASE
      CASE, ELSE
         LABEL,    "Wall", STD, LEFT, 140, 38, 1, 0, 0, 0, 0, 3
      ENDCASE

    ;******************************************************
    ; Interior Wall - Surface Properties Page
    ;******************************************************
;    MODDLG, 2514, 2514, 1, 170, 200, 175, 400, 0, "Interior Surface Properties", NOTIMP, 0, NOTIMP, 0
    TABPAGE, 3213, 2514, 1, 3, NOTIMP, " Surface Properties "

     LABEL, "This Side",  STD, CENTER, 240, 35, 1, 0, 0, 0, 12142, 3
     LABEL, "Other Side", STD, CENTER, 330, 35, 1, 0, 0, 0, 12385, 3
 
      EDIT, 12142, 12142,  753, 1, INTERIOR-WALL,  0,  INSIDE-SOL-ABS,  0, STD, 205,  55, 23, 70, 3, 3,    "Inside Solar Absorptance:",  LEFT, -170, 5, 0, LEFT, 4, 5, "Fraction of incident total solar radiation absorbed at the interior finish of this surface"
      EDIT, 12385, 12142,  753, 1, INTERIOR-WALL,  0,  INSIDE-SOL-ABS,  1, STD, 295,  55, 23, 70, 3, 3,                             "",  LEFT, -170, 5, 0, LEFT, 4, 5, "Fraction of incident total solar radiation absorbed at the interior finish of this surface"
      EDIT, 12143, 12143, 3006, 1, INTERIOR-WALL,  0, INSIDE-VIS-REFL,  0, STD, 205,  80, 23, 70, 3, 3,  "Inside Visible Reflectance:",  LEFT, -170, 5, 0, LEFT, 4, 5, "Fraction of the incident visible light reflected by the interior finish of this surface"
      EDIT, 12386, 12143, 3006, 1, INTERIOR-WALL,  0, INSIDE-VIS-REFL,  1, STD, 295,  80, 23, 70, 3, 3,                             "",  LEFT, -170, 5, 0, LEFT, 4, 5, "Fraction of the incident visible light reflected by the interior finish of this surface"
      EDIT, 12144, 12144,    0, 1, INTERIOR-WALL,  0,  SOLAR-FRACTION,  0, STD, 205, 105, 23, 70, 3, 3,       "Inside Solar Fraction:",  LEFT, -170, 5, 0, LEFT, 4, 5, "Fraction of solar radiation entering this space that is incident on the interior of this surface"
      EDIT, 12387, 12144,    0, 1, INTERIOR-WALL,  0,  SOLAR-FRACTION,  1, STD, 295, 105, 23, 70, 3, 3,                             "",  LEFT, -170, 5, 0, LEFT, 4, 5, "Fraction of solar radiation entering this space that is incident on the interior of this surface"


 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Underground Wall - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; AFR 6/24/09 - Dialog height was 460 now 550
 MODTABDLG, 3022, 3008, 1, 30, 30, 550, 440, 0, UNDERGROUND-WALL, "Underground Surface Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 12426, 3008, 0, 1, UNDERGROUND-WALL, 0, NAME,  0, STD, 175,  15, 400, 250, 19, 3, "Currently Active Surface:",  LEFT, -155, 5, 0, LEFT, 4, 5, "List of all underground surfaces defined in project; also allows library retrieval and creation"

    ;******************************************
    ; Underground Wall - Basic Specs Page
    ;******************************************
;    DATAWIN, 2014, 2014, 1, BLDG_FLR_UW, 135, -1
    TABPAGE, 3214, 2014, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 12139, 12139,     0, 1,  UNDERGROUND-WALL, 0,         NAME, -1, STD, 125,  10,  23, 250, 32, 3,  "Surface Name:",  LEFT, -95, 5, 0, LEFT, 4, 5, "Name of underground surface; right mouse quick menu options allow deleting, copying, linking and saving to library"

      COMBO, 15623, 15623,     0, 1,  UNDERGROUND-WALL, 0,       PARENT, -1, STD, 125,  65, 220, 250, 19, 3,  "Parent Space:",  LEFT, -95, 5, 0, LEFT, 4, 5, ""
      COMBO, 12487, 12736,     0, 1,  UNDERGROUND-WALL, 0, CONSTRUCTION, -1, STD, 125,  90, 220, 250, 19, 3,  "Construction:",  LEFT, -95, 5, 0, LEFT, 4, 5, "The construction (Layers) of the surface"
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
; NAVEDIT, 12163, 12091,     0, 1, 3135, UNDERGROUND-WALL, 0, CONSTRUCTION, -1, CONSTRUCTION, 0, U-VALUE, -1, STD, 325,  32,  21,  45,  3, 3, "U-Val:",  LEFT, 275,  34, 1, LEFT, 375,  34, "Overall thermal conductance of this construction (less exterior film resistance)"

       EDIT, 12162, 12162,     0, 1,  UNDERGROUND-WALL, 0,  U-EFFECTIVE, -1, STD, 125, 115,  23,  45,  4, 3,   "U-Effective:",  LEFT, -95, 5, 1, LEFT, 4, 5, "Effective u-value (used with custom weighting factors to estimate perimeter conduction)"

       EDIT, 12160, 12160,   769, 1,  UNDERGROUND-WALL, 0,   MULTIPLIER, -1, STD, 125, 140,  23,  45,  0, 3,    "Multiplier:",  LEFT, -95, 5, 0, LEFT, 4, 5, ""

; AFR 6/24/09 - moved everything below here down by 100
      LABEL, "Location & Geometry", STD, LEFT, 30, 278, 0, 0, 1, 375, 0, 3
      COMBO, 19056, 19056,   755, 1,  UNDERGROUND-WALL, 0,     LOCATION, -1, STD, 110, 300, 220, 265, 19, 3,      "Location:",  LEFT, -60, 5, 0, LEFT, 4, 5, "Positions this surface in the space (applies only if space is defined with Shape or Polygon)"
      COMBO, 19063,   694, 31030, 1,  UNDERGROUND-WALL, 0,      POLYGON, -1, STD, 110, 325, 220, 265, 19, 3,       "Polygon:",  LEFT, -60, 5, 0, LEFT, 4, 5, "Name of the Polygon that defines the surface's shape"

       EDIT, 19051, 19051,   755, 1,  UNDERGROUND-WALL, 0,            X, -1, STD, 110, 350,  23,  70,  2, 3,             "X:",  LEFT, -60, 5, 1, LEFT, 4, 5, "X coordinate for the surface origin (relative to this Space coordinate system)"
       EDIT, 19052, 19052,   755, 1,  UNDERGROUND-WALL, 0,            Y, -1, STD, 110, 375,  23,  70,  2, 3,             "Y:",  LEFT, -60, 5, 1, LEFT, 4, 5, "Y coordinate for the surface origin (relative to this Space coordinate system)"
       EDIT, 19053, 19053,   755, 1,  UNDERGROUND-WALL, 0,            Z, -1, STD, 110, 400,  23,  70,  2, 3,             "Z:",  LEFT, -60, 5, 1, LEFT, 4, 5, "Z coordinate for the surface origin (relative to this Space coordinate system)"
       EDIT, 19054, 19054,   755, 1,  UNDERGROUND-WALL, 0,      AZIMUTH, -1, STD, 110, 425,  23,  70,  2, 3,       "Azimuth:",  LEFT, -60, 5, 1, LEFT, 4, 5, "Azimuth of outward normal relative to Space Y-axis; before applying Tilt (positive = clockwise)"

       EDIT, 12161, 12161,     0, 1,  UNDERGROUND-WALL, 0,         AREA, -1, STD, 285, 350,  23,  74,  2, 3,          "Area:",  LEFT, -50, 5, 1, LEFT, 4, 5, "Area of this underground surface (an alternative to entering Height and Width)"
       EDIT, 19057, 19057,     0, 1,  UNDERGROUND-WALL, 0,       HEIGHT, -1, STD, 285, 375,  23,  74,  2, 3,        "Height:",  LEFT, -50, 5, 1, LEFT, 4, 5, "Dimension of the surface parallel to the Surface Y-axis (before applying a Tilt)"
       EDIT, 19058, 19058,     0, 1,  UNDERGROUND-WALL, 0,        WIDTH, -1, STD, 285, 400,  23,  74,  2, 3,         "Width:",  LEFT, -50, 5, 1, LEFT, 4, 5, "Width of the surface (measured parallel to the Surface x-axis)."
       EDIT, 19055, 19055,   755, 1,  UNDERGROUND-WALL, 0,         TILT, -1, STD, 285, 425,  23,  74,  2, 3,          "Tilt:",  LEFT, -50, 5, 1, LEFT, 4, 5, ""
 
      CASE, UNDERGROUND-WALL, 0, LOCATION, -1, =, 1, 1
         LABEL,  "Roof", STD, LEFT, 140, 38, 1, 0, 0, 0, 0, 3
      ENDCASE
      CASE, UNDERGROUND-WALL, 0, LOCATION, -1, =, 1, 2
         LABEL, "Floor", STD, LEFT, 140, 38, 1, 0, 0, 0, 0, 3
; AFR 6/24/09 - added the following edit boxes if LEED.
         EDIT, 19029, 19029,   0, 1,  UNDERGROUND-WALL, 0,          C-EXPOSED-PERIM, -1, STD, 260, 165,  23,  70,  2, 6, "Slab-on-Grade Exposed Perimeter:",  LEFT, -230, 5, 1, LEFT, 4, 5, "For slab-on-grade surfaces, perimeter length of slab within 10' of grade"
         EDIT, 19028, 19028,   0, 1,  UNDERGROUND-WALL, 0,                C-FFACTOR, -1, STD, 260, 190,  23,  70,  2, 6,          "Slab-on-Grade F-Factor:",  LEFT, -230, 5, 1, LEFT, 4, 5, "For slab-on-grade surfaces, ASHRAE F-factor"
      ENDCASE
      CASE, ELSE
         LABEL,  "Wall", STD, LEFT, 140, 38, 1, 0, 0, 0, 0, 3
; AFR 6/24/09 - added the following edit boxes if LEED.
         EDIT, 19029, 19029,   0, 1,  UNDERGROUND-WALL, 0,          C-EXPOSED-PERIM, -1, STD, 260, 165,  23,  70,  2, 6, "Slab-on-Grade Exposed Perimeter:",  LEFT, -230, 5, 1, LEFT, 4, 5, "For slab-on-grade surfaces, perimeter length of slab within 10' of grade"
         EDIT, 19031, 19031,   0, 1,  UNDERGROUND-WALL, 0,         C-FRAC-BELOW-GRD, -1, STD, 260, 190,  23,  70,  4, 6,    "Fraction of Wall Below-Grade:",  LEFT, -230, 5, 1, LEFT, 4, 5, "Fraction of underground wall height that is within 10' of grade"
         EDIT, 19028, 19028,   0, 1,  UNDERGROUND-WALL, 0,                C-FFACTOR, -1, STD, 260, 215,  23,  70,  2, 6,          "Slab-on-Grade F-Factor:",  LEFT, -230, 5, 1, LEFT, 4, 5, "For slab-on-grade surfaces, ASHRAE F-factor"
         EDIT, 19030, 19030,   0, 1,  UNDERGROUND-WALL, 0,                C-CFACTOR, -1, STD, 260, 240,  23,  70,  2, 6,       "Below-Grade Wall C-Factor:",  LEFT, -230, 5, 1, LEFT, 4, 5, "For below-grade wall surfaces, ASHRAE C-factor"
      ENDCASE

    ;******************************************************
    ; Underground Wall - Daylighting / Solar Page
    ;******************************************************
;    TABPAGE, 3023, 3006, 1, 3, "Daylighting"
;    TABPAGE, 3024, 3024, 1, 3, "Solar"
    TABPAGE, 3023, 3006, 1, 3, NOTIMP, " Daylighting  -  Solar "

      LABEL, "Daylighting",    STD, LEFT, 80,  18, 0, 0, 1, 330, 12084, 3
       EDIT, 12147, 12147, 3006, 1, UNDERGROUND-WALL, 0, INSIDE-VIS-REFL, -1, STD, 260,  40, 23, 70,  3, 3,  "Inside Visible Reflectance:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Fraction of the incident visible light reflected by the interior finish of this surface"
 
      LABEL, "Solar", STD, LEFT, 80,  88, 0, 0, 1, 330, 12085, 3
       EDIT, 12146, 12146,  753, 1, UNDERGROUND-WALL, 0,  INSIDE-SOL-ABS, -1, STD, 260, 110, 23, 70,  3, 3,    "Inside Solar Absorptance:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Fraction of incident total solar radiation absorbed at the interior finish of this surface"
       EDIT, 12148, 12148, 3024, 1, UNDERGROUND-WALL, 0,  SOLAR-FRACTION, -1, STD, 260, 135, 23, 70,  0, 3,       "Inside Solar Fraction:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Fraction of solar radiation entering this space that is incident on the interior of this surface"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Window - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; DATAWIN, 2006, 2006, 1, BLDG_FLR_XW_W, 135, -1
; MODTABDLG, 3012, 32012, 1, 100, 100, 235, 560, 0, "Exterior Surface - Window Properties", NOTIMP, 0, NOTIMP, 0
 MODTABDLG, 3012, 32012, 1, 30, 30, 470, 710, 0, WINDOW, "Window Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 12481, 32012, 0, 1, WINDOW, 0, NAME,  0, STD, 265,  15, 400, 250, 19, 3, "Currently Active Window:",  LEFT, -160, 5, 0, LEFT, 4, 5, "List of all windows defined in project; also allows library retrieval and creation"

    ;******************************************
    ; Window - Basic Specs Page
    ;******************************************
;    TABPAGE, 3090,   775, 1, 3, "Frame"
    TABPAGE, 3090, 32012, 1, 3, NOTIMP, " Basic Specs "

       EDIT, 12096, 12096, 32012, 1,  WINDOW, 0,             NAME, -1, STD, 120,   5,  23, 250, 32, 3,  "Window Name:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Name of window; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 12483, 12483, 32012, 1,  WINDOW, 0,           PARENT, -1, STD, 120,  30, 350, 250, 19, 3,  "Parent Wall:",  LEFT, -100, 5, 0, LEFT, 4, 5, ""
      COMBO, 18247, 12483, 32012, 1,  WINDOW, 0,      WINDOW-TYPE, -1, STD, 120,  55, 150, 250, 19, 3,"Type of Window:", LEFT, -100, 5, 0, LEFT, 4, 5, "The type of window - Standard or Skylight"
       EDIT, 12011, 12011,   769, 1,  WINDOW, 0,       MULTIPLIER, -1, STD, 120,  80,  23,  70,  0, 3,   "Multiplier:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Number of identical windows on this surface"
      COMBO, 18247, 12483, 32012, 1,  WINDOW, 0,  DIFFUSING-GLASS, -1, STD, 320,  80, 100,  50, 19, 3,    "Diffusing:", RIGHT,   -5, 5, 0, LEFT, 4, 5, "Whether or not the glazing is diffusing"

      LABEL, "Location & Geometry", STD, LEFT, 20, 108, 0, 0, 1, 265, 19022, 3
       EDIT, 19022, 19022,   788, 1,  WINDOW, 0,                X, -1, STD, 125, 130,  23,  70,  2, 3,            "X:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "X coordinate for the window origin (relative to this Surface coordinate system)"
       EDIT, 19023, 19023,   788, 1,  WINDOW, 0,                Y, -1, STD, 125, 155,  23,  70,  2, 3,            "Y:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Y coordinate for the window origin (relative to this Surface coordinate system)"
       EDIT, 19027, 19027,   776, 1,  WINDOW, 0,          SETBACK, -1, STD, 125, 180,  23,  70,  2, 3,      "Setback:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Distance that the window is recessed into the wall (shading effects only)"
       EDIT, 19024, 19024, 32012, 1,  WINDOW, 0,           HEIGHT, -1, STD, 125, 205,  23,  70,  2, 3,       "Height:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Dimension of the window parallel to the Surface Y-axis"
       EDIT, 19025, 19025, 32012, 1,  WINDOW, 0,            WIDTH, -1, STD, 125, 230,  23,  70,  2, 3,        "Width:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Width of the window (measured parallel to the Surface x-axis)."
       EDIT, 19025, 19025, 32012, 1,  WINDOW, 0,              WWR, -1, STD, 350, 130,  23,  70,  2, 3,  "Glazing Pct:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Percent Glazing"

      LABEL, "Window Frame", STD, LEFT, 20, 263, 0, 0, 1, 265, 12379, 3
       EDIT, 12379, 19026,   775, 1,  WINDOW, 0,      FRAME-WIDTH, -1, STD, 125, 285,  23,  70,  2, 3,  "Frame Width:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Width of window frame (assumed equal for all four sides of the window)"
       EDIT, 12380, 13137,   775, 1,  WINDOW, 0,    FRAME-CONDUCT, -1, STD, 125, 310,  23,  70,  3, 3,  "Conductance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Thermal conductance of the frame ( including the inside air film, excluding the outside airfilm)"
       EDIT, 12377, 13138,   775, 1,  WINDOW, 0,        FRAME-ABS, -1, STD, 125, 335,  23,  70,  3, 3,  "Absorptance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Fraction of total incident solar radiation absorbed by the outside surface of the frame"
      COMBO, 12378, 13139,   761, 1,  WINDOW, 0,      SPACER-TYPE, -1, STD, 125, 360, 120, 130, 19, 3,  "Spacer Type:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "The type of spacer that separates the glass layers (in multi-pane windows)"

      LABEL, "Window Glass/Layers", STD, LEFT, 395, 8, 0, 0, 1, 675, 12381, 3
      COMBO, 12381, 12381, 32012, 1,  WINDOW, 0,  WIN-SPEC-METHOD, -1, STD, 525,  30, 100, 150, 19, 3,  "Specification Method:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Glass Type Input = from library; Window Layers Input = custom defined using Layers"

    CASE,  WINDOW,  0, WINDOW-TYPE,  -1,  =, 1, 0
      CASE,  WINDOW, 0, WIN-SPEC-METHOD,  -1,  =, 1, 0
         COMBO, 18261, 19019, 760, 1, WINDOW, 0,       GLASS-TYPE, -1, STD, 525,  55, 250, 150, 19, 3,         "Type of Glass:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Glass type codes from either of two glass libraries (1 - 11 or 1000 - 9999, dbl click to edit)"
; SAC 5/31/07 - added access to WINDOW:C-USE-GTC
      CHECKBOX, 18320, 18320,   0, 1, WINDOW, 0,        C-USE-GTC,  0, STD, 395,  85,  17, 285,     7,  "Use Glass Library Component for Compliance",  RIGHT,   "Check if compliance analysis is to be performed using the glass library component (as opposed to using simplified window modeling characteristics)"
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;       NAVEDIT, 14280, 14280,   0, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0, TYPE, -1, STD, 500,  32,  21, 130,  2, 3, "Glazing Specification Method:",  LEFT, 305,  34, 0, LEFT, 530,  34, ""
;         CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 1
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;          NAVEDIT, 14299, 13131,   0, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0, GLASS-TYPE-CODE, -1, STD, 445,  82,  21,  55,  2, 3, "Library Selection:",  LEFT, 305,  84, 0, LEFT, 530,  59, "Amount of solar radiation that the window transmits (relative to standard glass)"
;           BUTTON, 10347, 2505,    0, 1, 2505, STD, 515,  57, 24, 115, 3, "Fins-Overhang...", "fin and overhang geometry"
;           BUTTON, 10348, 2509,    0, 1, 3132, STD, 515,  82, 24, 115, 3, "Library Details...", ""
;           BUTTON, 10349, 3013,    0, 1, 3090, STD, 515, 107, 24, 115, 3, "More...", "other window properties"
;         ENDCASE
;         CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 2
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;          NAVEDIT, 12014, 13132, 759, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0,  SHADING-COEF, -1, STD, 445,  82,  21,  55,  2, 3,      "Shading Coef:",  LEFT, 305,  84, 0, LEFT, 530,  59, "Amount of solar radiation that the window transmits (relative to standard glass)"
;          NAVEDIT, 14298, 13133, 759, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0, GLASS-CONDUCT, -1, STD, 445, 107,  21,  55,  2, 3, "Glass Conductance:",  LEFT, 305, 107, 0, LEFT, 530,  59, ""
;           BUTTON, 10215, 2505,    0, 1, 2505, STD, 515,  57, 24, 115, 3, "Fins-Overhang...", "fin and overhang geometry"
;           BUTTON, 10219, 2509,    0, 1, 3132, STD, 515,  82, 24, 115, 3, "Glass Details...", ""
;           BUTTON, 10214, 3013,    0, 1, 3090, STD, 515, 107, 24, 115, 3, "More...", "other window properties"
;         ENDCASE
      ENDCASE
      CASE,  WINDOW, 0, WIN-SPEC-METHOD,  -1,  =, 1, 1
        SPREAD, 18262, 11568, 0, 1, 0, PowerDOE, 0, WinStrSpread, 0, STD, 425,  55, 120, 250, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
;        BUTTON, 10216, 2505,    0, 1, 2505, STD, 510,  57, 24, 115, 3, "Fins-Overhang...", "fin and overhang geometry"
;        BUTTON, 10217, 3088,    0, 1, 3088, STD, 510,  82, 24, 115, 3, "Layers Details...", "window layers input"
;        BUTTON, 10218, 3013,    0, 1, 3090, STD, 510, 107, 24, 115, 3, "More...", "other window properties"
      ENDCASE
    ENDCASE

    CASE,  WINDOW,  0, WINDOW-TYPE,  -1,  =, 1, 1
      CASE,  WINDOW, 0, WIN-SPEC-METHOD,  -1,  =, 1, 0
         COMBO, 19156, 19019, 760, 1, WINDOW, 0,       GLASS-TYPE, -1, STD, 525,  55, 250, 150, 19, 3,         "Type of Glass:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Glass type codes from either of two glass libraries (1 - 11 or 1000 - 9999, dbl click to edit)"
; SAC 5/31/07 - added access to WINDOW:C-USE-GTC
      CHECKBOX, 18321, 18321,   0, 1, WINDOW, 0,        C-USE-GTC,  0, STD, 395,  85,  17, 285,     7,  "Use Glass Library Component for Compliance",  RIGHT,   "Check if compliance analysis is to be performed using the glass library component (as opposed to using simplified window modeling characteristics)"
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;       NAVEDIT, 14280, 14280,   0, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0, TYPE, -1, STD, 500,  32,  21, 130,  2, 3, "Glazing Specification Method:",  LEFT, 305,  34, 0, LEFT, 530,  34, ""
;         CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 1
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;          NAVEDIT, 14299, 13131,   0, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0, GLASS-TYPE-CODE, -1, STD, 445,  82,  21,  55,  2, 3, "Library Selection:",  LEFT, 305,  84, 0, LEFT, 530,  59, "Amount of solar radiation that the window transmits (relative to standard glass)"
;           BUTTON, 10347, 2505,    0, 1, 2505, STD, 515,  57, 24, 115, 3, "Fins-Overhang...", "fin and overhang geometry"
;           BUTTON, 10348, 2509,    0, 1, 3132, STD, 515,  82, 24, 115, 3, "Library Details...", ""
;           BUTTON, 10349, 3013,    0, 1, 3090, STD, 515, 107, 24, 115, 3, "More...", "other window properties"
;         ENDCASE
;         CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 2
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;          NAVEDIT, 12014, 13132, 759, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0,  SHADING-COEF, -1, STD, 445,  82,  21,  55,  2, 3,      "Shading Coef:",  LEFT, 305,  84, 0, LEFT, 530,  59, "Amount of solar radiation that the window transmits (relative to standard glass)"
;          NAVEDIT, 14298, 13133, 759, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0, GLASS-CONDUCT, -1, STD, 445, 107,  21,  55,  2, 3, "Glass Conductance:",  LEFT, 305, 107, 0, LEFT, 530,  59, ""
;           BUTTON, 10215, 2505,    0, 1, 2505, STD, 515,  57, 24, 115, 3, "Fins-Overhang...", "fin and overhang geometry"
;           BUTTON, 10219, 2509,    0, 1, 3132, STD, 515,  82, 24, 115, 3, "Glass Details...", ""
;           BUTTON, 10214, 3013,    0, 1, 3090, STD, 515, 107, 24, 115, 3, "More...", "other window properties"
;         ENDCASE
      ENDCASE
      CASE,  WINDOW, 0, WIN-SPEC-METHOD,  -1,  =, 1, 1
        SPREAD, 11568, 11568, 0, 1, 0, PowerDOE, 0, WinStrSpread, 0, STD, 425,  55, 120, 250, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
;        BUTTON, 10216, 2505,    0, 1, 2505, STD, 510,  57, 24, 115, 3, "Fins-Overhang...", "fin and overhang geometry"
;        BUTTON, 10217, 3088,    0, 1, 3088, STD, 510,  82, 24, 115, 3, "Layers Details...", "window layers input"
;        BUTTON, 10218, 3013,    0, 1, 3090, STD, 510, 107, 24, 115, 3, "More...", "other window properties"
      ENDCASE

; AFR 5/4/09 - moved skylight controls to Skylight tab
;      LABEL, "Skylight Surface", STD, LEFT, 280, 183, 0, 0, 1, 500, 12379, 3
;       EDIT, 18251, 19026,   775, 1,  WINDOW, 0,      DOME-DEPTH, -1, STD, 385, 205,  23,  70,  2, 3,     "Dome Depth:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Width of window frame (assumed equal for all four sides of the window)"
;       EDIT, 18252, 13137,   775, 1,  WINDOW, 0,SURFACE-RO-RATIO, -1, STD, 385, 255,  23,  70,  3, 3,"Surface/RO Area:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Thermal conductance of the frame ( including the inside air film, excluding the outside airfilm)"
;
;      LABEL, "Skylight Curb", STD, LEFT, 280, 288, 0, 0, 1, 500, 12379, 3
;       EDIT, 18248, 19026,   775, 1,  WINDOW, 0,      CURB-HEIGHT, -1, STD, 365, 310,  23,  70,  2, 3,  "Curb Height:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Width of window frame (assumed equal for all four sides of the window)"
;       EDIT, 18249, 13137,   775, 1,  WINDOW, 0,     CURB-CONDUCT, -1, STD, 365, 335,  23,  70,  3, 3,  "Conductance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Thermal conductance of the frame ( including the inside air film, excluding the outside airfilm)"
;       EDIT, 18250, 13138,   775, 1,  WINDOW, 0,         CURB-ABS, -1, STD, 365, 360,  23,  70,  3, 3,  "Absorptance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Fraction of total incident solar radiation absorbed by the outside surface of the frame"

    ENDCASE

    CASE,  WINDOW,  0, WINDOW-TYPE,  -1,  >, 1, 1
      CASE,  WINDOW, 0, WIN-SPEC-METHOD,  -1,  =, 1, 0
         COMBO, 18259, 19019, 760, 1, WINDOW, 0,       GLASS-TYPE, -1, STD, 525,  55, 250, 150, 19, 3,         "Type of Glass:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Glass type codes from either of two glass libraries (1 - 11 or 1000 - 9999, dbl click to edit)"
; SAC 5/31/07 - added access to WINDOW:C-USE-GTC
      CHECKBOX, 18322, 18322,   0, 1, WINDOW, 0,        C-USE-GTC,  0, STD, 395,  85,  17, 285,     7,  "Use Glass Library Component for Compliance",  RIGHT,   "Check if compliance analysis is to be performed using the glass library component (as opposed to using simplified window modeling characteristics)"
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;       NAVEDIT, 14280, 14280,   0, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0, TYPE, -1, STD, 500,  32,  21, 130,  2, 3, "Glazing Specification Method:",  LEFT, 305,  34, 0, LEFT, 530,  34, ""
;         CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 1
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;          NAVEDIT, 14299, 13131,   0, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0, GLASS-TYPE-CODE, -1, STD, 445,  82,  21,  55,  2, 3, "Library Selection:",  LEFT, 305,  84, 0, LEFT, 530,  59, "Amount of solar radiation that the window transmits (relative to standard glass)"
;           BUTTON, 10347, 2505,    0, 1, 2505, STD, 515,  57, 24, 115, 3, "Fins-Overhang...", "fin and overhang geometry"
;           BUTTON, 10348, 2509,    0, 1, 3132, STD, 515,  82, 24, 115, 3, "Library Details...", ""
;           BUTTON, 10349, 3013,    0, 1, 3090, STD, 515, 107, 24, 115, 3, "More...", "other window properties"
;         ENDCASE
;         CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 2
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;          NAVEDIT, 12014, 13132, 759, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0,  SHADING-COEF, -1, STD, 445,  82,  21,  55,  2, 3,      "Shading Coef:",  LEFT, 305,  84, 0, LEFT, 530,  59, "Amount of solar radiation that the window transmits (relative to standard glass)"
;          NAVEDIT, 14298, 13133, 759, 1, 3132, WINDOW, 0, GLASS-TYPE, -1, GLASS-TYPE, 0, GLASS-CONDUCT, -1, STD, 445, 107,  21,  55,  2, 3, "Glass Conductance:",  LEFT, 305, 107, 0, LEFT, 530,  59, ""
;           BUTTON, 10215, 2505,    0, 1, 2505, STD, 515,  57, 24, 115, 3, "Fins-Overhang...", "fin and overhang geometry"
;           BUTTON, 10219, 2509,    0, 1, 3132, STD, 515,  82, 24, 115, 3, "Glass Details...", ""
;           BUTTON, 10214, 3013,    0, 1, 3090, STD, 515, 107, 24, 115, 3, "More...", "other window properties"
;         ENDCASE
      ENDCASE
      CASE,  WINDOW, 0, WIN-SPEC-METHOD,  -1,  =, 1, 1
        SPREAD, 18260, 11568, 0, 1, 0, PowerDOE, 0, WinStrSpread, 0, STD, 425,  55, 120, 250, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
;        BUTTON, 10216, 2505,    0, 1, 2505, STD, 510,  57, 24, 115, 3, "Fins-Overhang...", "fin and overhang geometry"
;        BUTTON, 10217, 3088,    0, 1, 3088, STD, 510,  82, 24, 115, 3, "Layers Details...", "window layers input"
;        BUTTON, 10218, 3013,    0, 1, 3090, STD, 510, 107, 24, 115, 3, "More...", "other window properties"
      ENDCASE

; AFR 5/4/09 - moved skylight controls to Skylight tab
;      LABEL, "Skylight Surface", STD, LEFT, 280, 183, 0, 0, 1, 500, 12379, 3
;       EDIT, 18254, 19026,   775, 1,  WINDOW, 0,      DOME-DEPTH, -1, STD, 385, 205,  23,  70,  2, 3,     "Dome Depth:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Width of window frame (assumed equal for all four sides of the window)"
;       EDIT, 18263, 19026,   775, 1,  WINDOW, 0,   TUBE-DIAMETER, -1, STD, 385, 230,  23,  70,  2, 3,  "Tube Diameter:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Diameter of tube"
;       EDIT, 18255, 13137,   775, 1,  WINDOW, 0,SURFACE-RO-RATIO, -1, STD, 385, 255,  23,  70,  3, 3,"Surface/RO Area:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Thermal conductance of the frame ( including the inside air film, excluding the outside airfilm)"
;
;      LABEL, "Skylight Curb", STD, LEFT, 280, 288, 0, 0, 1, 500, 12379, 3
;       EDIT, 18256, 19026,   775, 1,  WINDOW, 0,      CURB-HEIGHT, -1, STD, 365, 310,  23,  70,  2, 3,  "Curb Height:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Width of window frame (assumed equal for all four sides of the window)"
;       EDIT, 18257, 13137,   775, 1,  WINDOW, 0,     CURB-CONDUCT, -1, STD, 365, 335,  23,  70,  3, 3,  "Conductance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Thermal conductance of the frame ( including the inside air film, excluding the outside airfilm)"
;       EDIT, 18258, 13138,   775, 1,  WINDOW, 0,         CURB-ABS, -1, STD, 365, 360,  23,  70,  3, 3,  "Absorptance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Fraction of total incident solar radiation absorbed by the outside surface of the frame"
;
;      LABEL, "Skylight Performance", STD, LEFT, 515, 183, 0, 0, 1, 675, 12379, 3
;       SPREAD, 18253, 11692, 0, 1, 0, PowerDOE, 0,  SkylightTRSpread,  0, STD, 515, 205, 180, 160, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
    ENDCASE

; AFR 5/4/09 - moved here from Compliance tab
; AFR 6/24/09 - changed the compliance flag for the next 5 controls to from 1 => 7, display only if non-LEED.
      COMBO, 15461,     0, 32012, 1,  WINDOW, 0,    C-PRODUCT-TYPE, -1, STD, 485, 183, 350, 190, 19, 7,     "Product Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "The type of fenestration product"
      COMBO, 15462,     0, 32012, 1,  WINDOW, 0,            C-TYPE, -1, STD, 485, 208, 350, 190, 19, 7,   "Product Source:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Select either site built or manufactured"
      COMBO, 15466,     0, 32012, 1,  WINDOW, 0,      C-FRAME-TYPE, -1, STD, 485, 233, 350, 190, 19, 7,       "Frame Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "The frame type for this fenestration product"
      COMBO, 15463,     0, 32012, 1,  WINDOW, 0,  C-UFACTOR-METHOD, -1, STD, 485, 258, 350, 190, 19, 7,  "U-factor Method:",  LEFT, -100, 5, 0, LEFT, 4, 5, "The method for determining the U-Factor of the fenestration product"
      COMBO, 15464,     0, 32012, 1,  WINDOW, 0,     C-SHGC-METHOD, -1, STD, 485, 283, 350, 190, 19, 7,      "SHGC Method:",  LEFT, -100, 5, 0, LEFT, 4, 5, "The method for determining the solar heat gain coefficient (SHGC) of the fenestration product"
      
; AFR 6/24/09 - the following two control display if a LEED compliance ruleset is loaded.
      COMBO, 19043,     0, 32012, 1,  WINDOW, 0,   C-901-PROD-TYPE, -1, STD, 485, 183, 350, 190, 19, 6,     "Product Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "ASHRAE fenestration product type"
      COMBO, 19044,     0, 32012, 1,  WINDOW, 0,  C-901-FRAME-TYPE, -1, STD, 485, 208, 350, 190, 19, 6,       "Frame Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "ASHREA frame type for vertical fenestration"
      
      
; SAC 12/22/00 - The following keywords were moved to the GLASS-TYPE command
;      COMBO, 15465,     0, 32012, 1,  WINDOW, 0,       C-NUM-PANES, -1, STD, 140, 190, 350, 190, 19, 1,  "Number of Panes:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Select the number of panes for this fenestration product"
;      COMBO, 15467,     0, 32012, 1,  WINDOW, 0,       C-AIR-SPACE, -1, STD, 140, 215, 350, 190, 19, 1,        "Air Space:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The size of the air space in a multiple paned fenestration product"
;      COMBO, 15468,     0, 32012, 1,  WINDOW, 0,   C-LOW-E-COATING, -1, STD, 140, 240, 350, 190, 19, 1,    "Low-E Coating:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Check if fenestration product has low-E coating"
;      COMBO, 15469,     0, 32012, 1,  WINDOW, 0,            C-TINT, -1, STD, 140, 265, 350, 190, 19, 1,             "Tint:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Check if fenestration product has tinted glass"

; AFR 6/24/09 - change dthe compliance flag for the next 7 controls to from 1 => 7, display only if non-LEED.
    CHECKBOX, 15471,     0, 32012, 1,  WINDOW, 0,        C-DIVIDERS, -1, STD, 485, 308,  17, 100,     7,          "Dividers", RIGHT,                         "Check if fenestration product has dividers between panes"
    CHECKBOX, 15472,     0, 32012, 1,  WINDOW, 0,   C-DIVIDED-LITES, -1, STD, 584, 308,  17, 100,     7,     "Divided Lites", RIGHT,                         "Check if fenestration product has true divided lites"

        EDIT, 15473,     0, 32012, 1,  WINDOW, 0,         C-UFACTOR, -1, STD, 340, 333,  23,  70,  2, 7,         "U-factor:",  LEFT,  -55, 5, 1, LEFT, 4, 5, "The NFRC certified U-Factor for this fenestration product"
        EDIT, 15476,     0, 32012, 1,  WINDOW, 0,  C-UFACTOR-CENTER, -1, STD, 570, 333,  23,  70,  2, 7,  "U-factor Center:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The NFRC certified U-Factor for this fenestration product"
        EDIT, 15474,     0, 32012, 1,  WINDOW, 0,            C-SHGC, -1, STD, 340, 358,  23,  70,  2, 7,             "SHGC:",  LEFT,  -55, 5, 1, LEFT, 4, 5, "The NFRC certified SHGC for this fenestration product"
        EDIT, 15475,     0, 32012, 1,  WINDOW, 0,     C-SHGC-CENTER, -1, STD, 570, 358,  23,  70,  2, 7,      "SHGC Center:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The manufacturers reported SHGC for the glass of this fenestration product"

    ;****************************************************************
    ; Window - Blinds-Drapes SwitchingPage
    ;****************************************************************
    TABPAGE, 3013,   762, 1, 3, NOTIMP, " Blinds/Drapes - Switching "
 
      COMBO, 17956,     0,  762, 1, WINDOW, 0,   WIN-SHADE-TYPE, -1, STD, 205,   5, 250, 160, 19, 3,                    "Shade Type:",  LEFT, -175, 5, 0, LEFT, 4, 5, "The type of shade that may be deployed on this window"
      COMBO, 12099, 12099,  762, 1, WINDOW, 0, SHADING-SCHEDULE, -1, STD, 520,   5, 250, 160, 19, 3,              "Shading Schedule:",  LEFT, -140, 5, 0, LEFT, 4, 5, "Schedule containing hourly multipliers applied to the solar transmission of this window"

      COMBO, 18977, 18977,  762, 1, WINDOW, 0,    MIN-SOLAR-SCH, -1, STD, 205,  30, 250, 160, 19, 3,        "Minimum Solar Schedule:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Schedule of minimum tolerable direct solar gain values (e.g., simulates closed blinds)"
      COMBO, 12103, 12103,  762, 1, WINDOW, 0,    MAX-SOLAR-SCH, -1, STD, 205,  55, 250, 160, 19, 3,        "Maximum Solar Schedule:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Schedule of maximum tolerable direct solar gain values (e.g., simulates closed blinds)"

      COMBO, 18238, 12103,  762, 1, WINDOW, 0,   MAX-SOLAR-CTRL, -1, STD, 520,  30, 180, 160, 19, 3,             "Max Solar Control:",  LEFT, -140, 5, 0, LEFT, 4, 5, "The variable used as the value to compate to the MAX-SOLAR-SCH to decide if the shade is closed"
      COMBO, 12104, 12104,  762, 1, WINDOW, 0,   OPEN-SHADE-SCH, -1, STD, 520,  55, 250, 160, 19, 3,           "Open Shade Schedule:",  LEFT, -140, 5, 0, LEFT, 4, 5, "Probability that a shade is re-opened when (beam & diffuse) solar gain decreases sufficiently"

      COMBO, 12113, 12113,  762, 1, WINDOW, 0, CONDUCT-TMIN-SCH, -1, STD, 205,  80, 250, 160, 19, 3,       "Conductance min-T Sched:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Schedule of minimum ambient temperatures (used to simulate movable insulation)"
      COMBO, 18976, 18976,  762, 1, WINDOW, 0, CONDUCT-TMAX-SCH, -1, STD, 205, 105, 250, 160, 19, 3,       "Conductance max-T Sched:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Schedule of maximum ambient temperatures (used to simulate movable insulation)"

       EDIT, 12107, 12107,  762, 1, WINDOW, 0,    SUN-CTRL-PROB, -1, STD, 610,  80,  23,  70,  3, 3,       "Sun Control Probability:",  LEFT, -230, 5, 1, LEFT, 4, 5, "Probability that an open shade will be closed when direct solar gain exceeds Maximum Glare"
      COMBO, 12112, 12112,  762, 1, WINDOW, 0, CONDUCT-SCHEDULE, -1, STD, 520, 105, 250, 160, 19, 3,          "Conductance Schedule:",  LEFT, -140, 5, 0, LEFT, 4, 5, "Schedule containing hourly multipliers for glass conductance properties for this window"

      COMBO, 12105, 12105,  753, 1, WINDOW, 0,    SOL-TRANS-SCH, -1, STD, 205, 130, 250, 160, 19, 3,     "Solar Transmittance Sched:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Schedule containing hourly solar transmission properties of shades (sunspaces only)"
      COMBO, 18283, 12105,  753, 1, WINDOW, 0,  DIRT-DEPREC-SCH, -1, STD, 205, 155, 250, 160, 19, 3,    "Dirt Depreciation Schedule:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Schedule containing hourly solar/viable transmission reduction due to dirt accumulation"
       EDIT, 12100, 12100,32012, 1, WINDOW, 0, SHADING-DIVISION, -1, STD, 610, 130,  23,  70,  0, 3,   "Number of Shading Divisions:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Number of 'vertical' segmentations used in shading calculations for this window"
       EDIT, 12114, 12114,32012, 1, WINDOW, 0,         INF-COEF, -1, STD, 610, 155,  23,  70,  3, 3,      "Infiltration Coefficient:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Infiltration flow coefficient for this window (used with the infiltration Crack Method)"

      LABEL, "Switching", STD, LEFT,  20, 193, 0, 0, 1, 675, 12116, 3
      COMBO, 12116, 12116,  774, 1, WINDOW, 0,   SWITCH-CONTROL, -1, STD, 205, 215, 250, 160, 19, 3,                 "Switch Control:",  LEFT, -175, 5, 0, LEFT, 4, 5, "For switchable glazings,  specifies how the switching is controlled"
      COMBO, 12115, 12115,  774, 1, WINDOW, 0,    GLASS-TYPE-SW, -1, STD, 205, 240, 250, 160, 19, 3,       "Glass Type When Switched:",  LEFT, -175, 5, 0, LEFT, 4, 5, "For switchable glazings,  name of the glass type for the fully switched state"
      COMBO, 12119, 12119,  774, 1, WINDOW, 0,       SWITCH-SCH, -1, STD, 490, 215, 250, 190, 19, 3,                "Switch Schedule:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Schedule that specifies when glass switching is allowed"
       EDIT, 12117, 12117,  774, 1, WINDOW, 0,    SWITCH-SET-LO, -1, STD, 490, 240,  23,  55,  1, 3,              "Switch Lo Setting:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Lower set point value for the selected window Switch Control variable"
       EDIT, 12118, 12118,  774, 1, WINDOW, 0,    SWITCH-SET-HI, -1, STD, 625, 240,  23,  55,  1, 3,                     "Hi Setting:", RIGHT,   -5, 5, 0, LEFT, 4, 5, "Upper set point value for the selected window Switch Control variable"
                                                                                                                                 
      LABEL, "Blind Data", STD, LEFT,  20, 280, 1, 0, 0, 365, 14522, 3
      COMBO, 14522,   768,  762, 1, WINDOW, 0,   BLIND-ADJ-TYPE, -1, STD, 205, 300, 120, 160, 19, 3,               "Adjustment Type:",  LEFT, -175, 5, 0, LEFT, 4, 5, ""
      COMBO, 14523,   767,  762, 1, WINDOW, 0,   BLIND-SCHEDULE, -1, STD, 205, 325, 250, 160, 19, 3,                      "Schedule:",  LEFT, -175, 5, 0, LEFT, 4, 5, ""
      COMBO, 14524,   766,  762, 1, WINDOW, 0,  BLIND-TRIGG-SCH, -1, STD, 205, 350, 250, 160, 19, 3,              "Trigger Schedule:",  LEFT, -175, 5, 0, LEFT, 4, 5, ""

      LABEL, "Slat Data",  STD, LEFT, 380, 280, 1, 0, 0, 675, 14525, 3
      COMBO, 14525,   765,  762, 1, WINDOW, 0,    SLAT-ADJ-TYPE, -1, STD, 520, 300, 120, 160, 19, 3,               "Adjustment Type:",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
      COMBO, 14526,   764,  762, 1, WINDOW, 0,    SLAT-SCHEDULE, -1, STD, 520, 325, 250, 160, 19, 3,                      "Schedule:",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
      COMBO, 14527,   763,  762, 1, WINDOW, 0,   SLAT-TRIGG-SCH, -1, STD, 520, 350, 250, 160, 19, 3,              "Trigger Schedule:",  LEFT, -130, 5, 0, LEFT, 4, 5, ""

; AFR 5/4/09 - added to hold skylight controls from the Basic Specs and Compliance Tabs
    ;****************************************************************
    ; Window - Skylighting
    ;****************************************************************
    TABPAGE, 3015,   762, 1, 3, NOTIMP, " Skylights "

      COMBO, 18247, 12483, 32012, 1,  WINDOW, 0,      WINDOW-TYPE, -1, STD, 120,  5, 150, 250, 19, 3,"Type of Window:", LEFT, -100, 5, 0, LEFT, 4, 5, "The type of window - Standard or Skylight"
      
      CASE,  WINDOW,  0, WINDOW-TYPE,  -1,  =, 1, 1

        LABEL, "Skylight Surface", STD, LEFT, 15, 38, 0, 0, 1, 235, 12379, 3
         EDIT, 18251, 19026,   775, 1,  WINDOW, 0,      DOME-DEPTH, -1, STD, 120, 60,  23,  70,  2, 3,     "Dome Depth:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Width of window frame (assumed equal for all four sides of the window)"
         EDIT, 18252, 13137,   775, 1,  WINDOW, 0,SURFACE-RO-RATIO, -1, STD, 120,110,  23,  70,  3, 3,"Surface/RO Area:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Thermal conductance of the frame ( including the inside air film, excluding the outside airfilm)"

        LABEL, "Skylight Curb", STD, LEFT, 15, 138, 0, 0, 1, 235, 12379, 3
         EDIT, 18248, 19026,   775, 1,  WINDOW, 0,      CURB-HEIGHT, -1, STD, 100, 165,  23,  70,  2, 3,  "Curb Height:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Width of window frame (assumed equal for all four sides of the window)"
         EDIT, 18249, 13137,   775, 1,  WINDOW, 0,     CURB-CONDUCT, -1, STD, 100, 190,  23,  70,  3, 3,  "Conductance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Thermal conductance of the frame ( including the inside air film, excluding the outside airfilm)"
         EDIT, 18250, 13138,   775, 1,  WINDOW, 0,         CURB-ABS, -1, STD, 100, 215,  23,  70,  3, 3,  "Absorptance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Fraction of total incident solar radiation absorbed by the outside surface of the frame"

      ENDCASE

      CASE,  WINDOW,  0, WINDOW-TYPE,  -1,  >, 1, 1

        LABEL, "Skylight Surface", STD, LEFT, 15, 38, 0, 0, 1, 235, 12379, 3
         EDIT, 18254, 19026,   775, 1,  WINDOW, 0,      DOME-DEPTH, -1, STD, 120,  60,  23,  70,  2, 3,     "Dome Depth:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Width of window frame (assumed equal for all four sides of the window)"
         EDIT, 18263, 19026,   775, 1,  WINDOW, 0,   TUBE-DIAMETER, -1, STD, 120,  85,  23,  70,  2, 3,  "Tube Diameter:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Diameter of tube"
         EDIT, 18255, 13137,   775, 1,  WINDOW, 0,SURFACE-RO-RATIO, -1, STD, 120, 110,  23,  70,  3, 3,"Surface/RO Area:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Thermal conductance of the frame ( including the inside air film, excluding the outside airfilm)"

        LABEL, "Skylight Curb", STD, LEFT, 15, 138, 0, 0, 1, 235, 12379, 3
         EDIT, 18256, 19026,   775, 1,  WINDOW, 0,      CURB-HEIGHT, -1, STD, 100, 165,  23,  70,  2, 3,  "Curb Height:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Width of window frame (assumed equal for all four sides of the window)"
         EDIT, 18257, 13137,   775, 1,  WINDOW, 0,     CURB-CONDUCT, -1, STD, 100, 190,  23,  70,  3, 3,  "Conductance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Thermal conductance of the frame ( including the inside air film, excluding the outside airfilm)"
         EDIT, 18258, 13138,   775, 1,  WINDOW, 0,         CURB-ABS, -1, STD, 100, 215,  23,  70,  3, 3,  "Absorptance:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Fraction of total incident solar radiation absorbed by the outside surface of the frame"

        LABEL, "Skylight Performance", STD, LEFT, 250, 38, 0, 0, 1, 405, 12379, 3
         SPREAD, 18253, 11692, 0, 1, 0, PowerDOE, 0,  SkylightTRSpread,  0, STD, 250, 60, 180, 160, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
      ENDCASE

    
    ;****************************************************************
    ; Window - Daylighting / Tubes
    ;****************************************************************
;    TABPAGE, 3014, 3006, 1, 3, "Daylighting"
;    TABPAGE, 3015, 3015, 1, 3, "Switching"
;    TABPAGE, 3016, 3016, 1, 3, "Other"
    TABPAGE, 3014, 3006, 1, 3, NOTIMP, " Daylighting - Light Well/Tube "
 
      LABEL, "Daylighting", STD, LEFT,  20,  3, 0, 0, 1, 675, 0, 3
      COMBO, 18284, 12106,  3006, 1, WINDOW, 0,    VIS-TRANS-SCH, -1, STD, 220,  20, 250, 200, 19, 3, "Visible Transmittance Schedule:",  LEFT, -190, 5, 0, LEFT, 4, 5, "Schedule of hourly multipliers applied to the visible transmission of this window"
       EDIT, 18285, 12108,   762, 1, WINDOW, 0,  GLARE-CTRL-PROB, -1, STD, 220,  45,  23,  70,  2, 3,      "Glare Control Probability:",  LEFT, -190, 5, 0, LEFT, 4, 5, "Probability that a shade is re-opened when (beam & diffuse) solar gain decreases sufficiently"
       EDIT, 18286, 12109,  3006, 1, WINDOW, 0,  INSIDE-VIS-REFL, -1, STD, 220,  70,  23,  70,  3, 3,     "Inside Visible Reflectance:",  LEFT, -190, 5, 0, LEFT, 4, 5, "Fraction of the incident visible light reflected by the interior surface of this window"
       EDIT, 18287, 12110,  3006, 1, WINDOW, 0,   DAY-X-DIVISION, -1, STD, 595,  20,  23,  65,  0, 3,         "Daylighting X Division:",  LEFT, -160, 5, 0, LEFT, 4, 5, "Number of 'vertical' segmentations used in direct daylight calculations for this window"
       EDIT, 18287, 12111,  3006, 1, WINDOW, 0,   DAY-Y-DIVISION, -1, STD, 595,  45,  23,  65,  0, 3,         "Daylighting Y Division:",  LEFT, -160, 5, 0, LEFT, 4, 5, "Number of 'horizontal' segmentations used in direct daylight calculations for this window"

      LABEL, "Light Well", STD, LEFT,  20, 98, 0, 0, 1, 675, 0, 3
      COMBO, 18289, 12106,  3006, 1, WINDOW, 0,       LIGHT-WELL, -1, STD, 220, 115, 250,  70, 19, 3,       "Is a Light Well Present?:",  LEFT, -190, 5, 0, LEFT, 4, 5, ""
      COMBO, 18290, 12106,  3006, 1, WINDOW, 0,  WELL-EFF-METHOD, -1, STD, 220, 140, 250, 130, 19, 3,           "Well Efficiency From:",  LEFT, -190, 5, 0, LEFT, 4, 5, ""
       EDIT, 18291, 12109,  3006, 1, WINDOW, 0,  WELL-EFFICIENCY, -1, STD, 220, 165,  23,  70,  3, 3,                "Well Efficiency:",  LEFT, -190, 5, 0, LEFT, 4, 5, ""
;future - D22 code not yet there
;      EDIT, 18292, 12109,  3006, 1, WINDOW, 0,   WELL-WALL-COND, -1, STD, 220, 190,  23,  70,  3, 3,               "Wall conductance:",  LEFT, -190, 5, 1, LEFT, 4, 5, ""
;     COMBO, 18293, 12106,  3006, 1, WINDOW, 0,     WELL-NEXT-TO, -1, STD, 220, 215, 250, 180, 19, 3,        "Otherside of Wall Space:",  LEFT, -190, 5, 0, LEFT, 4, 5, ""
       EDIT, 18294, 12110,  3006, 1, WINDOW, 0,       WELL-DEPTH, -1, STD, 595, 115,  23,  65,  3, 3,    "Depth (Ceiling to skylight):",  LEFT, -160, 5, 1, LEFT, 4, 5, ""
       EDIT, 18295, 12111,  3006, 1, WINDOW, 0,   WELL-WIDTH-BOT, -1, STD, 595, 140,  23,  65,  3, 3,         "Width at Ceiling Level:",  LEFT, -160, 5, 1, LEFT, 4, 5, ""
       EDIT, 18296, 12111,  3006, 1, WINDOW, 0,  WELL-LENGTH-BOT, -1, STD, 595, 165,  23,  65,  3, 3,        "Length at Ceiling Level:",  LEFT, -160, 5, 1, LEFT, 4, 5, ""
       EDIT, 18297, 12111,  3006, 1, WINDOW, 0, WELL-VIS-REFLECT, -1, STD, 595, 190,  23,  65,  3, 3,       "Wall Visible Reflectance:",  LEFT, -160, 5, 0, LEFT, 4, 5, ""
      
      LABEL, "Tubular Daylighting Device", STD, LEFT,  20,243, 0, 0, 1, 675, 18298, 3
      COMBO, 18298, 12106,  3006, 1, WINDOW, 0,  TUBE-EFF-METHOD, -1, STD, 220, 260, 250, 130, 19, 3,           "Tube Efficiency From:",  LEFT, -190, 5, 0, LEFT, 4, 5, ""
       EDIT, 18299, 12109,  3006, 1, WINDOW, 0,  TUBE-EFFICIENCY, -1, STD, 220, 285,  23,  70,  3, 3,                "Tube Efficiency:",  LEFT, -190, 5, 0, LEFT, 4, 5, ""
       EDIT, 18300, 12111,  3006, 1, WINDOW, 0,  TUBE-DIFF-TRANS, -1, STD, 220, 310,  23,  70,  3, 3,    "Tube Diffuser Transmittance:",  LEFT, -190, 5, 1, LEFT, 4, 5, ""
       EDIT, 18301, 12110,  3006, 1, WINDOW, 0,    TUBE-DIAMETER, -1, STD, 595, 260,  23,  65,  3, 3,                  "Tube Diameter:",  LEFT, -160, 5, 1, LEFT, 4, 5, ""
       EDIT, 18302, 12111,  3006, 1, WINDOW, 0,      TUBE-LENGTH, -1, STD, 595, 285,  23,  65,  3, 3,                    "Tube Length:",  LEFT, -160, 5, 1, LEFT, 4, 5, ""
       EDIT, 18303, 12111,  3006, 1, WINDOW, 0, TUBE-VIS-REFLECT, -1, STD, 595, 310,  23,  65,  3, 3,       "Tube Visible Reflectance:",  LEFT, -160, 5, 0, LEFT, 4, 5, ""
      
;future - D22 code not yet there
;     LABEL, "Window Solar Gain Distribution", STD, LEFT,  30,338, 0, 0, 1, 675, 0, 3
;     COMBO, 18304, 12106,  3006, 1, WINDOW, 0,       SOLHEAT-TO, -1, STD, 220, 355, 250, 200, 19, 3,  "Space Getting Balance of Heat:",  LEFT, -190, 5, 0, LEFT, 4, 5, ""
;      EDIT, 18305, 12111,  3006, 1, WINDOW, 0, SOLHEAT-TO-SPACE, -1, STD, 595, 355,  23,  65,  3, 3,       "Fraction to Parent Space:",  LEFT, -160, 5, 0, LEFT, 4, 5, ""
    
    ;****************************************************************                                                                         
    ; Window - Fins & Overhang Dialog                                                                              
    ;****************************************************************
; MODDLG, 2505, 32033, 1, 20, 85, 400, 600, 0, "Window Fins & Overhang", NOTIMP, 0, NOTIMP, 0
    TABPAGE, 3016, 32033, 1, 3, NOTIMP, " Fins  -  Overhang "

   PICTURE, 29005, 29005, 0, 1, PowerDOE, 0, Constant, 0, 115, 15, 188, 475, 3, 0, 1, 255, 255, 255, 100, 101
;   LABEL, "(Fin/Overhang Diagram Goes Here)", STD, CENTER, 352, 90, 1, 0, 0, 0, 0, 3
;    RECT, 20, 200, 80, 625, -1, -1, -1, 1, 120, 120, 120, 0, 0, 1, 0, 0, 3

   LABEL, "Left Fin", STD, LEFT, 20, 223, 1, 0, 0, 205, 0, 3
    EDIT, 12215, 12215, 32033, 1, WINDOW,  0,     LEFT-FIN-D, -1, STD, 135, 245, 23, 50, 1, 3,       "Depth (LD):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Depth of the left fin (the dimension of either of the projecting edges)"
    EDIT, 12213, 12213, 32033, 1, WINDOW,  0,     LEFT-FIN-A, -1, STD, 135, 270, 23, 50, 1, 3,  "Horz Space (LA):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Distance between the left edge of the window and the edge of the left fin"
    EDIT, 12214, 12214, 32033, 1, WINDOW,  0,     LEFT-FIN-B, -1, STD, 135, 295, 23, 50, 1, 3,  "Vert Space (LB):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Distance between left fin top edge and window top edge, (-) fin extends above window"
    EDIT, 12216, 12216, 32033, 1, WINDOW,  0,     LEFT-FIN-H, -1, STD, 135, 320, 23, 50, 1, 3,      "Height (LH):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Height of the left fin (measured parallel to the Window Y-axis)"
 
   LABEL, "Overhang", STD, LEFT, 250, 223, 1, 0, 0, 445, 0, 3
    EDIT, 12219, 12219, 32033, 1, WINDOW,  0,     OVERHANG-D, -1, STD, 365, 245, 23, 50, 1, 3,       "Depth (OD):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Depth of the overhang (the dimension of both of the projecting edges)"
    EDIT, 12217, 12217, 32033, 1, WINDOW,  0,     OVERHANG-A, -1, STD, 365, 270, 23, 50, 1, 3,  "Horz Space (OA):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Distance overhang extends beyond the LEFT edge of the window"
    EDIT, 12218, 12218, 32033, 1, WINDOW,  0,     OVERHANG-B, -1, STD, 365, 295, 23, 50, 1, 3,  "Vert Space (OB):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Distance between the top of the window and the bottom of the overhang"
    EDIT, 12220, 12220, 32033, 1, WINDOW,  0,     OVERHANG-W, -1, STD, 365, 320, 23, 50, 1, 3,       "Width (OW):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Width of the overhang (measured parallel to the Window X-axis)"
    EDIT, 12221, 12221, 32033, 1, WINDOW,  0, OVERHANG-ANGLE, -1, STD, 365, 345, 23, 50, 1, 3,     "Angle (OAng):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Angle of the overhang relative to the window plane (e.g., <90° tilts 'down',  >90° tilts 'up')"

   LABEL, "Right Fin", STD, LEFT, 490, 223, 1, 0, 0, 675, 0, 3
    EDIT, 12224, 12224, 32033, 1, WINDOW,  0,    RIGHT-FIN-D, -1, STD, 605, 245, 23, 50, 1, 3,       "Depth (RD):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Depth of the right fin (the dimension of both of the projecting edges)"
    EDIT, 12222, 12222, 32033, 1, WINDOW,  0,    RIGHT-FIN-A, -1, STD, 605, 270, 23, 50, 1, 3,  "Horz Space (RA):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Distance between the right edge of the window and the edge of the right fin"
    EDIT, 12223, 12223, 32033, 1, WINDOW,  0,    RIGHT-FIN-B, -1, STD, 605, 295, 23, 50, 1, 3,  "Vert Space (RB):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Distance between right fin top edge and window top edge, (-) fin extends above window"
    EDIT, 12225, 12225, 32033, 1, WINDOW,  0,    RIGHT-FIN-H, -1, STD, 605, 320, 23, 50, 1, 3,      "Height (RH):",  LEFT, -105, 5, 1, LEFT, 4, 5, "Height of the right fin (measured parallel to the door Y-axis)"

; AFR 5/4/09 - moved to Basic Specs per Kevin/Luke
;    ;******************************************
;    ; Window - Compliance Page
;    ;******************************************
;    TABPAGE, 3226, 32012, 1, 1, NOTIMP, " Compliance "
;
;      COMBO, 15461,     0, 32012, 1,  WINDOW, 0,    C-PRODUCT-TYPE, -1, STD, 140,  40, 350, 190, 19, 1,     "Product Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The type of fenestration product"
;      COMBO, 15462,     0, 32012, 1,  WINDOW, 0,            C-TYPE, -1, STD, 140,  65, 350, 190, 19, 1,   "Product Source:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Select either site built or manufactured"
;      COMBO, 15466,     0, 32012, 1,  WINDOW, 0,      C-FRAME-TYPE, -1, STD, 140,  90, 350, 190, 19, 1,       "Frame Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The frame type for this fenestration product"
;      COMBO, 15463,     0, 32012, 1,  WINDOW, 0,  C-UFACTOR-METHOD, -1, STD, 140, 115, 350, 190, 19, 1,  "U-factor Method:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The method for determining the U-Factor of the fenestration product"
;      COMBO, 15464,     0, 32012, 1,  WINDOW, 0,     C-SHGC-METHOD, -1, STD, 140, 140, 350, 190, 19, 1,      "SHGC Method:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The method for determining the solar heat gain coefficient (SHGC) of the fenestration product"
;; SAC 12/22/00 - The following keywords were moved to the GLASS-TYPE command
;;      COMBO, 15465,     0, 32012, 1,  WINDOW, 0,       C-NUM-PANES, -1, STD, 140, 190, 350, 190, 19, 1,  "Number of Panes:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Select the number of panes for this fenestration product"
;;      COMBO, 15467,     0, 32012, 1,  WINDOW, 0,       C-AIR-SPACE, -1, STD, 140, 215, 350, 190, 19, 1,        "Air Space:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The size of the air space in a multiple paned fenestration product"
;;      COMBO, 15468,     0, 32012, 1,  WINDOW, 0,   C-LOW-E-COATING, -1, STD, 140, 240, 350, 190, 19, 1,    "Low-E Coating:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Check if fenestration product has low-E coating"
;;      COMBO, 15469,     0, 32012, 1,  WINDOW, 0,            C-TINT, -1, STD, 140, 265, 350, 190, 19, 1,             "Tint:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Check if fenestration product has tinted glass"
;
;   CHECKBOX, 15470,     0, 32012, 1,  WINDOW, 0,      C-GLASS-DOOR, -1, STD, 141, 168,  17, 150,     1,        "Glass Door", RIGHT,                         "Check if this fenestration product is a glass door"
;   CHECKBOX, 15471,     0, 32012, 1,  WINDOW, 0,        C-DIVIDERS, -1, STD, 141, 193,  17, 150,     1,          "Dividers", RIGHT,                         "Check if fenestration product has dividers between panes"
;   CHECKBOX, 15472,     0, 32012, 1,  WINDOW, 0,   C-DIVIDED-LITES, -1, STD, 141, 218,  17, 150,     1,     "Divided Lites", RIGHT,                         "Check if fenestration product has true divided lites"
;
;       EDIT, 15473,     0, 32012, 1,  WINDOW, 0,         C-UFACTOR, -1, STD, 140, 240,  23,  70,  2, 1,         "U-factor:",  LEFT,  -110, 5, 1, LEFT, 4, 5, "The NFRC certified U-Factor for this fenestration product"
;       EDIT, 15474,     0, 32012, 1,  WINDOW, 0,            C-SHGC, -1, STD, 140, 265,  23,  70,  2, 1,             "SHGC:",  LEFT,  -110, 5, 1, LEFT, 4, 5, "The NFRC certified SHGC for this fenestration product"
;       EDIT, 15475,     0, 32012, 1,  WINDOW, 0,     C-SHGC-CENTER, -1, STD, 140, 290,  23,  70,  2, 1,      "SHGC Center:",  LEFT,  -110, 5, 1, LEFT, 4, 5, "The manufacturers reported SHGC for the glass of this fenestration product"
;
;; SAC 5/31/07 - added access to WINDOW:C-USE-GTC
;   CHECKBOX, 18323, 18323,     0, 1,  WINDOW, 0,         C-USE-GTC,  0, STD,  30, 340,  17, 335,     1,  "Use Glass Library Component in Compliance Analysis",  RIGHT,   "Check if compliance analysis is to be performed using the glass library component (as opposed to using simplified window modeling characteristics)"
;
;; SAC 9/23/03 - Added new section for skylight daylighting related controls
;   LABEL, "Skylight Light Well", STD, LEFT, 460, 43, 1, 0, 0, 668, 0, 3
;       EDIT, 15465,     0, 32012, 1,  WINDOW, 0,      C-WELL-DEPTH, -1, STD, 585,  65,  23,  70,  2, 1,       "Well Depth:",  LEFT,  -110, 5, 1, LEFT, 4, 5, "Skylight light well depth"
;       EDIT, 15467,     0, 32012, 1,  WINDOW, 0,     C-WELL-HEIGHT, -1, STD, 585,  90,  23,  70,  2, 1,      "Well Length:",  LEFT,  -110, 5, 1, LEFT, 4, 5, "Skylight light well length of opening"
;       EDIT, 15468,     0, 32012, 1,  WINDOW, 0,      C-WELL-WIDTH, -1, STD, 585, 115,  23,  70,  2, 1,       "Well Width:",  LEFT,  -110, 5, 1, LEFT, 4, 5, "Skylight light well width of opening"
;       EDIT, 15469,     0, 32012, 1,  WINDOW, 0,  C-WELL-WALL-REFL, -1, STD, 585, 140,  23,  70,  3, 1, "Wall Reflectance:",  LEFT,  -110, 5, 1, LEFT, 4, 5, "Skylight light well wall reflectance"
;       EDIT, 15476,     0, 32012, 1,  WINDOW, 0,   C-WELL-TOP-REFL, -1, STD, 585, 165,  23,  70,  3, 1,  "Top Reflectance:",  LEFT,  -110, 5, 1, LEFT, 4, 5, "Skylight light well top reflectance"
;
;; Either Prescribed or reserved for future use
;;  66> C-SINGLE-DOUBLE      "-- unused --"           "Check if this window is double glazed"
;;  75> C-FEN-SPEC-METH      "Fenestration Method:"   "The simulation method for fenestration product"
;;  80> C-IS-SKYLIGHT        "Skylight"               "Checked if fenestration product is a skylight"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Door - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; DATAWIN, 2008, 2008, 1, BLDG_FLR_XW_D, 135, -1
; MODTABDLG, 3017, 3008, 1, 100, 100, 110, 350, 0, "Exterior Surface - Door Properties", NOTIMP, 0, NOTIMP, 0
 MODTABDLG, 3017, 3008, 1, 30, 30, 470, 710, 0, DOOR, "Door Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 12489,  2008, 0, 1, DOOR, 0, NAME,  0, STD, 265,  15, 400, 250, 19, 3, "Currently Active Door:",  LEFT, -145, 5, 0, LEFT, 4, 5, "List of all doors defined in project; also allows library retrieval and creation"

    ;******************************************************
    ; Door - Basic Specs Page
    ;******************************************************
;    TABPAGE, 3020, 3020, 1, 3, "Construction"
    TABPAGE, 3020, 2008, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 12097, 12097,     0, 1,  DOOR, 0,             NAME, -1, STD, 120,  10,  23, 250, 32, 3,    "Door Name:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Name of door; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 12483, 12483,     0, 1,  DOOR, 0,           PARENT, -1, STD, 120,  40, 350, 250, 19, 3,  "Parent Wall:",  LEFT, -100, 5, 0, LEFT, 4, 5, ""

       EDIT, 12152, 12152,   769, 1,  DOOR, 0,       MULTIPLIER, -1, STD, 480,  10,  23,  40,  0, 3,   "Multiplier:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Number of identical doors on this surface"

      LABEL, "Location & Geometry", STD, LEFT, 50, 83, 0, 0, 1, 265, 19022, 3
       EDIT, 19034, 19034,   788, 1,  DOOR, 0,                X, -1, STD, 135, 105,  23,  70,  2, 3,            "X:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "X coordinate for the door origin (relative to this Surface coordinate system)"
       EDIT, 19035, 19035,   788, 1,  DOOR, 0,                Y, -1, STD, 135, 130,  23,  70,  2, 3,            "Y:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Y coordinate for the door origin (relative to this Surface coordinate system)"
       EDIT, 19038, 19038,   776, 1,  DOOR, 0,          SETBACK, -1, STD, 135, 155,  23,  70,  2, 3,      "Setback:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "The distance that the door is recessed into the wall (shading effects only)"
       EDIT, 19036, 19036,     0, 1,  DOOR, 0,           HEIGHT, -1, STD, 135, 180,  23,  70,  2, 3,       "Height:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Dimension of the door parallel to the Surface Y-axis"
       EDIT, 19037, 19037,     0, 1,  DOOR, 0,            WIDTH, -1, STD, 135, 205,  23,  70,  2, 3,        "Width:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Width of the door (measured parallel to the Surface x-axis)."

      LABEL, "Construction", STD, LEFT, 350, 83, 0, 0, 1, 645, 12153, 3
      COMBO, 12153,  3020,     0, 1,  DOOR, 0,     CONSTRUCTION, -1, STD, 440, 105, 250, 205, 19, 3, "Construction:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "The construction (Layers) of the door"

; AFR 6/24/09 - added compliance section for LEED
      LABEL, "Compliance Information", STD, LEFT, 350, 143, 0, 0, 1, 645, 12153, 6
      COMBO, 19040,  19040,     0, 1,  DOOR, 0,     C-TYPE, -1, STD, 440, 165, 250, 205, 19, 6, "Door Type:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "ASHRAE door type"

; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;       EDIT, 12127, 12093, 0, 1, CONSTRUCTION, 0, ABSORPTANCE, -1, STD, 190,  20, 21, 70, 3, 3, "Absorptance:", RIGHT, 175, 23, 0, LEFT, 183, 23, "Fraction of incident solar radiation absorbed by the exterior finish of this construction"
;       EDIT, 12128, 12128, 0, 1, CONSTRUCTION, 0,   ROUGHNESS, -1, STD, 190,  45, 21, 70, 0, 3,   "Roughness:", RIGHT, 175, 48, 0, LEFT, 183, 48, ""
;       EDIT, 12129, 12091, 0, 1, CONSTRUCTION, 0,     U-VALUE, -1, STD, 190,  70, 21, 70, 3, 3,     "U-Value:", RIGHT, 175, 73, 1, LEFT, 263, 73, "Overall thermal conductance of this construction (less exterior film resistance)"

;  BUTTON, 10220, 3018,    0, 1, 3018, STD, 485,   7, 24, 115, 3, "Shading-View", ""
;  BUTTON, 10222, 2511,    0, 1, 2511, STD, 485,  32, 24, 115, 3, "Fins-Overhang", ""
;  BUTTON, 10323, 3006,    0, 1, 3019, STD, 485,  57, 24, 115, 3, "Daylighting", ""
;  BUTTON, 10223, 3020,    0, 1, 3020, STD, 485,  82, 24, 115, 3, "Construction", ""
;  BUTTON, 10221, 3021,    0, 1, 3021, STD, 485, 107, 24, 115, 3, "Other Properties", ""

    ;****************************************************************
    ; Door - Shading / View  -  Daylighting  -  Other Page
    ;****************************************************************
;    TABPAGE, 3018, 3018, 1, 3, "Shading & View"
;    TABPAGE, 3019, 3006, 1, 3, "Daylighting"
;    TABPAGE, 3021, 3021, 1, 3, "Other"
    TABPAGE, 3018, 3018, 1, 3, NOTIMP, " Shading / View  -  Daylighting  -  Other "

      LABEL, "Shading / View", STD, LEFT, 225,  48, 0, 0, 1, 470, 12120, 3
       EDIT, 12120, 12120,     0, 1, DOOR, 0, SHADING-DIVISION, -1, STD, 400,  70, 23, 70, 0, 3, "Number of Shading Divisions:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Number of 'vertical' segmentations used in shading calculations for this door"      

      LABEL, "Daylighting",    STD, LEFT, 225, 133, 0, 0, 1, 470, 12126, 3
       EDIT, 12126, 12126,  3006, 1, DOOR, 0,  INSIDE-VIS-REFL, -1, STD, 400, 155, 23, 70, 3, 3,  "Inside Visible Reflectance:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Fraction of the incident visible light reflected by the interior finish of this door"
 
      LABEL, "Other Data",     STD, LEFT, 225, 218, 0, 0, 1, 470, 12123, 3
       EDIT, 12123, 12123,     0, 1, DOOR, 0,         INF-COEF, -1, STD, 400, 240, 23, 70, 1, 3,    "Infiltration Coefficient:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Infiltration flow coefficient for this door (used with the infiltration Crack Method)"
       EDIT, 12125, 12125,     0, 1, DOOR, 0,    INSIDE-ABSORP, -1, STD, 400, 265, 23, 70, 3, 3,          "Inside Absorptance:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Fraction of incident total solar radiation absorbed at the interior finish of this surface"


    ;****************************************************************
    ; Bldg - Floor - Exterior Wall - Door Fins-Overhang Dialog
    ;****************************************************************
; MODDLG, 2511, 32033, 1, 20, 85, 400, 600, 0, "Door Fins & Overhang", NOTIMP, 0, NOTIMP, 0
    TABPAGE, 3021, 32033, 1, 3, NOTIMP, " Fins  -  Overhang "

   LABEL, "(Fin/Overhang Diagram Goes Here)", STD, CENTER, 352, 90, 1, 0, 0, 0, 0, 3
; TO DO ?? - implement new graphic control - perhaps using JPGs?
;   METAFILE, 29006, 29006, 0, 1, PowerDOE, 0, Constant, 0, 15, 15, 185, 560, 1, 1, 100

   LABEL, "Left Fin", STD, LEFT, 30, 223, 1, 0, 0, 205, 0, 3
    EDIT, 12228, 12228, 32033, 1, DOOR,  0,     LEFT-FIN-D, -1, STD, 130, 245, 23, 55, 1, 3,       "Depth (D):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Depth of the left fin (the dimension of either of the projecting edges)"
    EDIT, 12226, 12226, 32033, 1, DOOR,  0,     LEFT-FIN-A, -1, STD, 130, 270, 23, 55, 1, 3,  "Horz Space (A):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Distance between the left edge of the door and the edge of the left fin"
    EDIT, 12227, 12227, 32033, 1, DOOR,  0,     LEFT-FIN-B, -1, STD, 130, 295, 23, 55, 1, 3,  "Vert Space (B):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Distance between left fin top edge and door top edge, (-) fin extends above door"
    EDIT, 12229, 12229, 32033, 1, DOOR,  0,     LEFT-FIN-H, -1, STD, 130, 320, 23, 55, 1, 3,      "Height (H):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Height of the left fin (measured parallel to the door Y-axis)"
 
   LABEL, "Overhang", STD, LEFT, 260, 223, 1, 0, 0, 445, 0, 3
    EDIT, 12232, 12232, 32033, 1, DOOR,  0,     OVERHANG-D, -1, STD, 360, 245, 23, 55, 1, 3,       "Depth (D):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Depth of the overhang (the dimension of both of the projecting edges)"
    EDIT, 12230, 12230, 32033, 1, DOOR,  0,     OVERHANG-A, -1, STD, 360, 270, 23, 55, 1, 3,  "Horz Space (A):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Distance overhang extends beyond the LEFT edge of the door"
    EDIT, 12231, 12231, 32033, 1, DOOR,  0,     OVERHANG-B, -1, STD, 360, 295, 23, 55, 1, 3,  "Vert Space (B):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Distance between the top of the door and the bottom of the overhang"
    EDIT, 12233, 12233, 32033, 1, DOOR,  0,     OVERHANG-W, -1, STD, 360, 320, 23, 55, 1, 3,       "Width (W):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Width of the overhang (measured parallel to the door X-axis)"
    EDIT, 12234, 12234, 32033, 1, DOOR,  0, OVERHANG-ANGLE, -1, STD, 360, 345, 23, 55, 1, 3,           "Angle:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Angle of the overhang relative to the door plane (e.g., <90° tilts 'down',  >90° tilts 'up')"

   LABEL, "Right Fin", STD, LEFT, 500, 223, 1, 0, 0, 675, 0, 3
    EDIT, 12237, 12237, 32033, 1, DOOR,  0,    RIGHT-FIN-D, -1, STD, 600, 245, 23, 55, 1, 3,       "Depth (D):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Depth of the right fin (the dimension of both of the projecting edges)"
    EDIT, 12235, 12235, 32033, 1, DOOR,  0,    RIGHT-FIN-A, -1, STD, 600, 270, 23, 55, 1, 3,  "Horz Space (A):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Distance between the right edge of the door and the edge of the right fin"
    EDIT, 12236, 12236, 32033, 1, DOOR,  0,    RIGHT-FIN-B, -1, STD, 600, 295, 23, 55, 1, 3,  "Vert Space (B):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Distance between right fin top edge and door top edge, (-) fin extends above door"
    EDIT, 12238, 12238, 32033, 1, DOOR,  0,    RIGHT-FIN-H, -1, STD, 600, 320, 23, 55, 1, 3,      "Height (H):",  LEFT, -100, 5, 1, LEFT, 4, 5, "Height of the right fin (measured parallel to the door Y-axis)"



 ;********************************************************************
 ;********************************************************************
 ;**
 ;**     Polygon Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************

 MODTABDLG, 3162, 999, 1, 30, 30, 380, 440, 0, POLYGON, "Polygon Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 19018, 19018, 0, 1, POLYGON, 0, NAME,  0, STD, 175,  15, 400, 250, 19, 3, "Currently Active Polygon:",  LEFT, -155, 5, 0, LEFT, 4, 5, "List of all polygons defined in project; also allows library retrieval and creation"

    ;******************************************
    ; Polygon - Basic Specs Page
    ;******************************************
    TABPAGE, 3163, 31030, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 13075, 13075,     0, 1,  POLYGON, 0,             NAME, -1, STD, 125,  10,  23, 270, 32, 3,  "Polygon Name:",  LEFT, -95, 5, 0, LEFT, 4, 5, "Name of polygon; right mouse quick menu options allow deleting, copying, linking and saving to library"

     SPREAD, 11516, 11516, 0, 1, 0, PowerDOE, 0, PolySpread, 0, STD, 70, 50, 215, 285, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""

; TO DO - Integrate Button class and handle these special functions
;    ;-----------------------------------------------------------------------------------------------------------------------;
;    ;----  WARNING:  CHANGING THE ID OF THIS SPREADSHEET CONTROL WILL PREVENT THE INSERT/REMOVE FUNCTIONS FROM WORKING  ----;
;    ;-----------------------------------------------------------------------------------------------------------------------;
;  BUTTON, 10277, 10277, 0, 1, 31870, STD,  20,  230, 24, 125, 3, "Insert Vertex", ""      
;  BUTTON, 10278, 10278, 0, 1, 31871, STD, 150,  230, 24, 125, 3, "Remove Vertex", ""      



 ;********************************************************************
 ;********************************************************************
 ;**
 ;**     Construction / Layers / Materials Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************

; MODTABDLG, 3073, 3008, 1, 100, 100, 360, 600, 0, "Surface Construction, Layers, and Material Data", NOTIMP, 0, NOTIMP, 0
 MODTABDLG, 3073, 3008, 1, 30, 30, 480, 760, 0, NOTIMP, "Surface Construction, Layers, and Material Properties", NOTIMP, 0, NOTIMP, 0

   ;*****************************************
   ; Constructions Page
   ;*****************************************
   TABPAGE, 3135,  3136, 1, 3, CONSTRUCTION, " Construction "

     COMBO, 13046, 13046, 0, 1, CONSTRUCTION, 0, NAME,  0, STD, 270,   5, 400, 250, 19, 3, "Currently Active Construction:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all constructions defined in project; also allows library retrieval and creation"
     STATIC, 1, CONSTRUCTION, 0, TYPE, 0, 0, 0, 540, 10, 175, STD, LEFT, "Type: ",   "", 0, 3

      LINE,  20, 40, 735, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     LABEL, "Surface Construction Parameters", STD, LEFT, 30, 58, 1, 0, 0, 280, 0, 3
      EDIT,    12133, 12133, 0, 1, CONSTRUCTION, 0,             NAME, -1, STD, 115,  80,  23, 165, 32, 3,                "Construction:", LEFT,  -85, 5, 0, LEFT, 4, 5, "Name of construction; right mouse quick menu options allow deleting, copying, linking and saving to library"
     COMBO,    14469, 14469, 0, 1, CONSTRUCTION, 0,             TYPE, -1, STD, 160, 105,  80, 120, 19, 3,        "Specification Method:", LEFT, -130, 5, 0, LEFT, 4, 5, "Whether you define all of the Layers (& Materials) in the wall, or just its overall parameters"

     CASE,  CONSTRUCTION,  0, TYPE,  -1, = 1, 1
         EDIT, 14563, 12091, 0, 0, CONSTRUCTION, 0,          U-VALUE, -1, STD, 160, 130,  23,  60,  3, 3,          "Calculated U-Value:", LEFT, -130, 5, 1, LEFT, 4, 5, "Overall thermal conductance of this construction (less exterior film resistance)"
         EDIT, 12092, 12092, 0, 1, CONSTRUCTION, 0,        ROUGHNESS, -1, STD, 160, 155,  23,  60,  0, 3,           "Surface Roughness:", LEFT, -130, 5, 1, LEFT, 4, 5, ""
         EDIT, 12093, 12093, 0, 1, CONSTRUCTION, 0,      ABSORPTANCE, -1, STD, 160, 180,  23,  60,  3, 3,       "Ext. Color (absorpt.):", LEFT, -130, 5, 1, LEFT, 4, 5, "Fraction of incident solar radiation absorbed by the exterior finish of this construction"

;; SAC 10/20/00
;         EDIT, 15415, 15415, 0, 1, CONSTRUCTION, 0,   C-USER-INP-ABS, -1, STD, 165, 205,  23,  70,  2, 1,                 "Absorptance:", LEFT, -135, 5, 1, LEFT, 4, 5, "The absorptance of the exterior surface"
;        COMBO, 15610, 15610, 0, 1, CONSTRUCTION, 0,      C-WALL-TYPE, -1, STD, 165, 230, 200, 130, 19, 1,           "Construction Type:", LEFT, -135, 5, 0, LEFT, 4, 5, "The basic construction type"
;         EDIT, 15416, 15416, 0, 1, CONSTRUCTION, 0, C-FORM-THREE-REF, -1, STD, 165, 255,  23, 400, 76, 1,            "Form 3 Reference:", LEFT, -135, 5, 0, LEFT, 4, 5, "Title of CEC Nonres Form 3 for this assembly"
; SAC 12/27/05 - moved C- keywords (above) into new compliance section of dialog (below)

; SAC 12/27/05 - Added new compliance section to handle new T-24-2005 keywords
; AFR 6/30/09 - removed compliance information for LEED.
       LABEL, "Compliance Information", STD, LEFT, 325, 58,  1, 0, 0, 725, 0, 7
; SAC 1/6/10 - removed keywords no longer referenced by T24-08 ruleset (C-WALL-TYPE & C-USER-INP-ABS)
;           COMBO, 15610, 15610, 0, 1, CONSTRUCTION, 0,      C-WALL-TYPE, -1, STD, 420,  80, 200, 120, 19, 7,                 "Const. Type:", LEFT,  -85, 5, 0, LEFT, 4, 5, "The basic construction type"
;            EDIT, 15415, 15415, 0, 1, CONSTRUCTION, 0,   C-USER-INP-ABS, -1, STD, 420, 105,  23,  70,  2, 7,                 "Absorptance:", LEFT,  -85, 5, 1, LEFT, 4, 5, "The absorptance of the exterior surface"
        CHECKBOX, 17894,     0, 0, 1, CONSTRUCTION, 0,      C-USE-TABLE, -1, STD, 335, 135,  17, 175,     7,        "Use Energy Code Table", RIGHT,                        ""
           COMBO, 17895,     0, 0, 1, CONSTRUCTION, 0,          C-TABLE, -1, STD, 420, 155, 200, 120, 19, 7,                       "Table:", LEFT,  -60, 5, 0, LEFT, 4, 5, ""
           COMBO, 17896,     0, 0, 1, CONSTRUCTION, 0,            C-ROW, -1, STD, 420, 180, 200, 120, 19, 7,                         "Row:", LEFT,  -60, 5, 0, LEFT, 4, 5, ""
           COMBO, 17897,     0, 0, 1, CONSTRUCTION, 0,         C-COLUMN, -1, STD, 420, 205, 200, 120, 19, 7,                      "Column:", LEFT,  -60, 5, 0, LEFT, 4, 5, ""

            EDIT, 17898,     0, 0, 1, CONSTRUCTION, 0,      C-THICKNESS, -1, STD, 660,  80,  23,  50,  1, 7,                   "Thickness:", LEFT,  -95, 5, 1, LEFT, 4, 5, ""
            EDIT, 17899,     0, 0, 1, CONSTRUCTION, 0,  C-INS-THICKNESS, -1, STD, 660, 105,  23,  50,  1, 7,             "Insul Thickness:", LEFT,  -95, 5, 1, LEFT, 4, 5, ""
           COMBO, 17900,     0, 0, 1, CONSTRUCTION, 0,        C-FURRING, -1, STD, 615, 130, 200, 110, 19, 7,                     "Furring:", LEFT,  -50, 5, 0, LEFT, 4, 5, ""

          LABEL, "R-values (h-ft2-°F/Btu):", STD, LEFT, 565, 162,  1, 0, 0, 725, 0, 7
            EDIT, 17901,     0, 0, 1, CONSTRUCTION, 0,     C-INS-RVALUE, -1, STD, 665, 180,  23,  60,  2, 7,                  "Insulation:", LEFT,  -75, 5, 0, LEFT, 4, 5, ""
            EDIT, 17902,     0, 0, 1, CONSTRUCTION, 0, C-RIGID-INS-RVAL, -1, STD, 665, 205,  23,  60,  2, 7,                 "Rigid Insul:", LEFT,  -75, 5, 0, LEFT, 4, 5, ""
            EDIT, 17903,     0, 0, 1, CONSTRUCTION, 0,   C-FURRING-RVAL, -1, STD, 665, 230,  23,  60,  2, 7,                     "Furring:", LEFT,  -75, 5, 0, LEFT, 4, 5, ""

            EDIT, 15416, 15416, 0, 1, CONSTRUCTION, 0, C-FORM-THREE-REF, -1, STD, 420, 260,  23, 305, 76, 7,                 "Form 3 Ref.:", LEFT,  -85, 5, 0, LEFT, 4, 5, "Title of CEC Nonres Form 3 for this assembly"

           COMBO, 18318, 19017, 0, 1, CONSTRUCTION, 0,  WALL-PARAMETERS, -1, STD, 120, 280, 250, 160, 19, 3,             "Wall Parameters:", LEFT,  -90, 5, 0, LEFT, 4, 5, "Name of the wall parameters for this construction (Sunspace/Trombe wall parameters)"
           COMBO, 19017, 19017, 0, 1, CONSTRUCTION, 0,           LAYERS, -1, STD, 160, 305, 250, 200, 19, 3,         "Construction Layers:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of the construction of this wall (alternative to U-Value)"

        CASE,  CONSTRUCTION,  0, LAYERS,  -1, !=, 1, 0
           LABEL, "(material layers ordered from outside to inside)", STD, LEFT, 375, 310, 1, 0, 0, 0, 19017, 3
          SPREAD, 11505, 11505, 0, 1, 0, PowerDOE, 0, ConsSpread, 0, STD, 30, 330, 110, 695, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""

;         NAVEDIT, 12132, 12132, 0, 1, 3136, LAYERS, 0, INSIDE-FILM-RES, -1, STD, 205, 305, 21, 50, 3, 3, "Inside Film Resistance (R-val):", LEFT,  14, 5, 0, LEFT, 4, 5, ""

; TO DO - need to port the GRAPH control and migrate it to Olectra Chart
;           LABEL, "Heat Transfer From Outside To Inside", STD, LEFT, 345,  58, 1, 0, 0, 675, 0, 3
;           LABEL, "(Heat Transfer graph goes here)", STD, CENTER, 510, 130, 1, 0, 0, 590, 0, 3
;           GRAPH, 29021, 29021, 0, 1, PowerDOE, 0, GraphCons, -1, 290,  70, 135, 300, 1, 0
                                                              
;          RADIOFIRST, 29018, 29018, 0, 1, 29021, PowerDOE, 0, ConsGraphOutIn,  0, 0, STD, 195, 361, 18, 89, 3,  "Out To In", RIGHT, "Graph heat flow from outside to inside"
;          RADIONEXT,  29019, 29018, 0, 1, 29021, PowerDOE, 0, ConsGraphOutOut, 0, 1, STD, 195, 379, 18, 89, 3, "Out To Out", RIGHT, "Graph heat flow from outside to outside"
;          RADIONEXT,  29020, 29018, 0, 1, 29021, PowerDOE, 0, ConsGraphInIn,   0, 2, STD, 195, 397, 18, 89, 3,   "In To In", RIGHT, "Graph heat flow from inside to inside"
       ENDCASE
     ENDCASE

     CASE,  CONSTRUCTION,  0, TYPE,  -1, = 1, 2
         EDIT, 12091, 12091, 0, 1, CONSTRUCTION, 0,          U-VALUE, -1, STD, 160, 130,  23,  60,  3, 3,             "Overall U-Value:", LEFT, -130, 5, 1, LEFT, 4, 5, "Overall thermal conductance of this construction (less exterior film resistance)"
         EDIT, 14408, 12092, 0, 1, CONSTRUCTION, 0,        ROUGHNESS, -1, STD, 160, 155,  23,  60,  0, 3,           "Surface Roughness:", LEFT, -130, 5, 1, LEFT, 4, 5, ""
         EDIT, 14446, 12093, 0, 1, CONSTRUCTION, 0,      ABSORPTANCE, -1, STD, 160, 180,  23,  60,  3, 3,       "Ext. Color (absorpt.):", LEFT, -130, 5, 1, LEFT, 4, 5, "Fraction of incident solar radiation absorbed by the exterior finish of this construction"

;; SAC 10/20/00
;         EDIT, 15417, 15415, 0, 1, CONSTRUCTION, 0,   C-USER-INP-ABS, -1, STD, 165, 205,  23,  70,  3, 1,         "User Input Absorpt.:", LEFT, -135, 5, 1, LEFT, 4, 5, ""
;        COMBO, 15611, 15610, 0, 1, CONSTRUCTION, 0,      C-WALL-TYPE, -1, STD, 165, 230, 200, 130, 19, 1,           "Construction Type:", LEFT, -135, 5, 0, LEFT, 4, 5, "The basic construction type"
;         EDIT, 15418, 15416, 0, 1, CONSTRUCTION, 0, C-FORM-THREE-REF, -1, STD, 165, 255,  23, 400, 76, 1,              "Form Three Ref:", LEFT, -135, 5, 0, LEFT, 4, 5, ""
; SAC 12/27/05 - moved C- keywords (above) into new compliance section of dialog (below)

; SAC 12/27/05 - Added new compliance section to handle new T-24-2005 keywords
; AFR 6/30/09 - removed compliance information for LEED.
        LABEL, "Compliance Information", STD, LEFT, 325, 58,  1, 0, 0, 725, 0, 7
; SAC 1/6/10 - removed keywords no longer referenced by T24-08 ruleset (C-WALL-TYPE & C-USER-INP-ABS)
;            COMBO, 15611, 15610, 0, 1, CONSTRUCTION, 0,      C-WALL-TYPE, -1, STD, 420,  80, 200, 120, 19, 7,                 "Const. Type:", LEFT,  -85, 5, 0, LEFT, 4, 5, "The basic construction type"
;             EDIT, 15417, 15415, 0, 1, CONSTRUCTION, 0,   C-USER-INP-ABS, -1, STD, 420, 105,  23,  70,  2, 7,                 "Absorptance:", LEFT,  -85, 5, 1, LEFT, 4, 5, "The absorptance of the exterior surface"
         CHECKBOX, 17904,     0, 0, 1, CONSTRUCTION, 0,      C-USE-TABLE, -1, STD, 335, 135,  17, 175,     7,        "Use Energy Code Table", RIGHT,                        ""
            COMBO, 17905,     0, 0, 1, CONSTRUCTION, 0,          C-TABLE, -1, STD, 420, 155, 200, 120, 19, 7,                       "Table:", LEFT,  -60, 5, 0, LEFT, 4, 5, ""
            COMBO, 17906,     0, 0, 1, CONSTRUCTION, 0,            C-ROW, -1, STD, 420, 180, 200, 120, 19, 7,                         "Row:", LEFT,  -60, 5, 0, LEFT, 4, 5, ""
            COMBO, 17907,     0, 0, 1, CONSTRUCTION, 0,         C-COLUMN, -1, STD, 420, 205, 200, 120, 19, 7,                      "Column:", LEFT,  -60, 5, 0, LEFT, 4, 5, ""

             EDIT, 17908,     0, 0, 1, CONSTRUCTION, 0,      C-THICKNESS, -1, STD, 660,  80,  23,  50,  1, 7,                   "Thickness:", LEFT,  -95, 5, 1, LEFT, 4, 5, ""
             EDIT, 17909,     0, 0, 1, CONSTRUCTION, 0,  C-INS-THICKNESS, -1, STD, 660, 105,  23,  50,  1, 7,             "Insul Thickness:", LEFT,  -95, 5, 1, LEFT, 4, 5, ""
            COMBO, 17910,     0, 0, 1, CONSTRUCTION, 0,        C-FURRING, -1, STD, 615, 130, 200, 110, 19, 7,                     "Furring:", LEFT,  -50, 5, 0, LEFT, 4, 5, ""

           LABEL, "R-values (h-ft2-°F/Btu):", STD, LEFT, 565, 162,  1, 0, 0, 725, 0, 7
             EDIT, 17911,     0, 0, 1, CONSTRUCTION, 0,     C-INS-RVALUE, -1, STD, 665, 180,  23,  60,  2, 7,                  "Insulation:", LEFT,  -75, 5, 0, LEFT, 4, 5, ""
             EDIT, 17912,     0, 0, 1, CONSTRUCTION, 0, C-RIGID-INS-RVAL, -1, STD, 665, 205,  23,  60,  2, 7,                 "Rigid Insul:", LEFT,  -75, 5, 0, LEFT, 4, 5, ""
             EDIT, 17913,     0, 0, 1, CONSTRUCTION, 0,   C-FURRING-RVAL, -1, STD, 665, 230,  23,  60,  2, 7,                     "Furring:", LEFT,  -75, 5, 0, LEFT, 4, 5, ""

             EDIT, 15418, 15416, 0, 1, CONSTRUCTION, 0, C-FORM-THREE-REF, -1, STD, 420, 260,  23, 305, 76, 7,                 "Form 3 Ref.:", LEFT,  -85, 5, 0, LEFT, 4, 5, "Title of CEC Nonres Form 3 for this assembly"

            COMBO, 18319, 19017, 0, 1, CONSTRUCTION, 0,  WALL-PARAMETERS, -1, STD, 120, 280, 250, 160, 19, 3,             "Wall Parameters:", LEFT,  -90, 5, 0, LEFT, 4, 5, "Name of the wall parameters for this construction (Sunspace/Trombe wall parameters)"
     ENDCASE

   ;*****************************************
   ; Layers Page
   ;*****************************************
   TABPAGE, 3136, 3136, 1, 3, LAYERS, " Layers "

     COMBO, 13006, 13006, 0, 1, LAYERS, 0,            NAME,  0, STD, 270,   5, 400, 250, 19, 3, "Currently Active Layers:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all layers defined in project; also allows library retrieval and creation"
      LINE,  20, 40, 735, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
   
      EDIT, 13122, 13122, 0, 1, LAYERS, 0,            NAME, -1, STD,  80,  60,  23, 200, 32, 3,                         "Layers:", LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of layers; right mouse quick menu options allow deleting, copying, linking and saving to library"
      EDIT, 13123, 12132, 0, 1, LAYERS, 0, INSIDE-FILM-RES, -1, STD, 220,  85,  23,  60,  3, 3, "Inside Film Resistance (R-val):", LEFT, -190, 5, 0, LEFT, 4, 5, ""
      
     LABEL, "Material Layers (ordered from outside to inside):", STD, LEFT, 30, 120, 1, 0, 0, 725, 0, 3
    SPREAD, 11520, 11520, 0, 1, 0, PowerDOE, 0, LayersSpread, 0, STD, 30, 140, 250, 695, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""

   ;******************************************
   ;  Material Tab
   ;******************************************
   TABPAGE, 3137, 3136, 1, 3, MATERIAL, " Material "
 
     COMBO, 13032, 13032, 0, 1, MATERIAL, 0,            NAME,  0, STD, 270,   5, 400, 250, 19, 3, "Currently Active Building Material:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all materials defined in project; also allows library retrieval and creation"
     STATIC, 1, MATERIAL, 0, TYPE, 0, 0, 0, 540, 10, 175, STD, LEFT, "Type: ",   "", 0, 3

      LINE,  20, 40, 735, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

      EDIT, 13124, 13124, 0, 1, MATERIAL, 0,          NAME, -1, STD, 280,  70,  23, 200, 32, 3,             "Material:", LEFT,  -60, 5, 0, LEFT, 4, 5, "Name of layers; right mouse quick menu options allow deleting, copying, linking and saving to library"
     COMBO, 14470, 14470, 0, 1, MATERIAL, 0,          TYPE, -1, STD, 355, 100,  80, 125, 19, 3, "Specification Method:", LEFT, -135, 5, 0, LEFT, 4, 5, ""

     LABEL, "Material Properties:", STD, LEFT, 240, 148, 1, 0, 0, 480, 0, 3
     CASE,  MATERIAL,  0, TYPE,  -1, = 1, 1
      EDIT, 13125, 13125, 0, 1, MATERIAL, 0,     THICKNESS, -1, STD, 355, 170,  23,  65,  3, 3,     "Thickness:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 13126, 13126, 0, 1, MATERIAL, 0,  CONDUCTIVITY, -1, STD, 355, 195,  23,  65,  4, 3,  "Conductivity:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 13127, 13127, 0, 1, MATERIAL, 0,       DENSITY, -1, STD, 355, 220,  23,  65,  2, 3,       "Density:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 13128, 13128, 0, 1, MATERIAL, 0, SPECIFIC-HEAT, -1, STD, 355, 245,  23,  65,  3, 3, "Specific Heat:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
     ENDCASE
   
     CASE,  MATERIAL,  0, TYPE,  -1, = 1, 2
      EDIT, 13129, 13129, 0, 1, MATERIAL, 0,    RESISTANCE, -1, STD, 355, 170,  23,  65,  3, 3,    "Resistance:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
     ENDCASE


 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Wall Parameters - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

 MODTABDLG, 3360, 3008, 1, 30, 30, 480, 440, 0, WALL-PARAMETERS, "Wall Parameters Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 12402, 3008, 0, 1, WALL-PARAMETERS, 0, NAME,  0, STD, 190,  15, 400, 250, 19, 3, "Currently Active Wall Parameters:",  LEFT, -180, 5, 0, LEFT, 4, 5, "List of all Wall Parameters defined in project"

    ;******************************************
    ; Wall Parameters - Sunspace Int Wall page
    ;******************************************
    TABPAGE, 3361, 2004, 1, 3, NOTIMP, " Sunspace Interior Walls "

       EDIT, 17875, 12095,     0, 1,  WALL-PARAMETERS, 0,            NAME, -1, STD, 125,  10,  23, 250, 32, 3,  "Parameters Name:",  LEFT, -95, 5, 0, LEFT, 4, 5, "Name of wall parameters right mouse quick menu options allow deleting, copying, linking and saving to library"
      LABEL, "Sunspace Interior Wall Properties", STD, LEFT, 30, 75, 0, 0, 1, 35, 0, 3
      COMBO, 17876,   694, 31030, 1,  WALL-PARAMETERS, 0,   AIR-FLOW-TYPE, -1, STD, 170, 100, 220, 125, 19, 3,   "Air Flow Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Sunspace Interior Wall Air Flow Type"
       EDIT, 17877, 12001,   769, 1,  WALL-PARAMETERS, 0, LOWER-VENT-AREA, -1, STD, 170, 125,  23,  70,  2, 3, "Lower Vent Area:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Sunspace Interior Wall Lower Vent Area"
       EDIT, 17878, 19008,   755, 1,  WALL-PARAMETERS, 0, UPPER-VENT-AREA, -1, STD, 170, 150,  23,  70,  2, 3, "Upper Vent Area:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Sunspace Interior Wall Upper Vent Area"
       EDIT, 17879, 19009,   755, 1,  WALL-PARAMETERS, 0,   VERT-VENT-SEP, -1, STD, 170, 175,  23,  70,  2, 3, "Vent Seperation:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Sunspace Interior Wall Vertical Vent Seperation"
       EDIT, 17880, 19010,   755, 1,  WALL-PARAMETERS, 0,   AIR-FLOW-RATE, -1, STD, 170, 200,  23,  70,  2, 3,   "Air Flow Rate:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Sunspace Interior Wall Air Flow Rate"
       EDIT, 17881, 19011,   755, 1,  WALL-PARAMETERS, 0,AIR-FLOW-CTRL-DT, -1, STD, 170, 225,  23,  70,  2, 3, "Flow Control DT:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Sunspace Interior Wall Air Flow Control Delta T"
       EDIT, 17882, 19013,     0, 1,  WALL-PARAMETERS, 0,     FAN-KW/FLOW, -1, STD, 170, 250,  23,  70,  2, 3,"Air Flow kW/Flow:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Sunspace Interior Wall kW/Flow"
       EDIT, 17883, 19014,     0, 1,  WALL-PARAMETERS, 0,       DOORWAY-H, -1, STD, 170, 275,  23,  70,  2, 3,  "Doorway Height:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Sunspace Interior Wall Doorway Height"
       EDIT, 17884, 19012,     0, 1,  WALL-PARAMETERS, 0,       DOORWAY-W, -1, STD, 170, 300,  23,  70,  2, 3,   "Doorway Width:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Sunspace Interior Wall Doorway Width"
 

    ;****************************************************************
    ; Wall Parameters - Trombe Wall page
    ;****************************************************************
    TABPAGE, 3362, 3006, 1, 3, NOTIMP, " Trombe Walls "
 
       EDIT, 17875, 12095,    0, 1,   WALL-PARAMETERS, 0,            NAME, -1, STD, 125,  10, 23, 250, 32, 3,  "Parameters Name:",  LEFT, -95, 5, 0, LEFT, 4, 5, "Name of wall parameters right mouse quick menu options allow deleting, copying, linking and saving to library"
      LABEL, "Trombe Wall Properties",    STD, LEFT, 30,  75, 0, 0, 1, 35, 12084, 3
       EDIT, 17885, 12084, 3006, 1,   WALL-PARAMETERS, 0,      EMISSIVITY, -1, STD, 170, 100, 23, 70,  3, 3, "Outside Emissivity:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Trombe Wall Outside Wall Emissivity"
       EDIT, 17886, 12088, 3010, 1,   WALL-PARAMETERS, 0,   CHANNEL-WIDTH, -1, STD, 170, 125, 23, 70,  3, 3,      "Channel Width:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Trombe Wall Channel Width"

 
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Glass Type Tabbed Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
 MODTABDLG, 3131, 32012, 1, 30, 30, 470, 710, 0, GLASS-TYPE, "Glass Type Properties", NOTIMP, 0, NOTIMP, 0
 
    COMBO, 14330, 14330, 0, 1, GLASS-TYPE, 0, NAME, -1, STD, 230, 15, 400, 250, 19, 3, "Currently Active Glass Type:", RIGHT, -10, 5, 0, LEFT, 4, 5, "List of all glass types defined in project; also allows library retrieval and creation"
    STATIC, 1, GLASS-TYPE, 0, TYPE, 0, 0, 0, 500, 20, 175, STD, LEFT, "Type: ",   "", 0, 3

   ;******************************************
   ;  General Tab
   ;******************************************
   TABPAGE, 3132,   760, 1, 3, NOTIMP, " Basic Specifications "
   
     EDIT,    14350, 14350, 0, 1, GLASS-TYPE, 0,            NAME,  0, STD, 110,  10,  23, 200, 32, 3,            "Glass Type:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Name of glass type; right mouse quick menu options allow deleting, copying, linking and saving to library"
    COMBO,    14355, 14280, 0, 1, GLASS-TYPE, 0,            TYPE,  0, STD, 165,  40, 110, 145, 19, 3,  "Specification Method:",  LEFT, -135, 5, 0, LEFT, 4, 5, "The type of layer (Glass, Gap or Blind)"

; SAC 12/22/00 - Added new compliance Glass Type keywords
    LABEL, "Compliance Information", STD, LEFT, 355, 93,  1, 0, 0, 670, 0, 1
; AFR 6/24/09 - all the following have compliance flag = 7, display when compliance ruleset, and non-LEED    
      COMBO, 15600,     0,     0, 1,  GLASS-TYPE, 0,    C-PRODUCT-TYPE, -1, STD, 480, 115, 350, 190, 19, 7,     "Product Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The type of fenestration product"
      COMBO, 15601,     0,     0, 1,  GLASS-TYPE, 0,            C-TYPE, -1, STD, 480, 140, 350, 190, 19, 7,   "Product Source:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Select either site built or manufactured"
      COMBO, 15602,     0,     0, 1,  GLASS-TYPE, 0,       C-NUM-PANES, -1, STD, 480, 165, 350, 190, 19, 7,  "Number of Panes:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Select the number of panes for this fenestration product"
      COMBO, 15603,     0,     0, 1,  GLASS-TYPE, 0,       C-AIR-SPACE, -1, STD, 480, 190, 350, 190, 19, 7,        "Air Space:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The size of the air space in a multiple paned fenestration product"
; AFR 5/4/09 - removed      
;      COMBO, 15604,     0,     0, 1,  GLASS-TYPE, 0,   C-LOW-E-COATING, -1, STD, 480, 215, 350, 190, 19, 7,    "Low-E Coating:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Description of fenestration product's low-E coating"
; AFR 5/4/09 - moved up
      COMBO, 15605,     0,     0, 1,  GLASS-TYPE, 0,            C-TINT, -1, STD, 480, 215, 350, 190, 19, 7,             "Tint:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Description of fenestration product's tint"
; AFR 5/4/09 - removed      
;      COMBO, 15609,     0,     0, 1,  GLASS-TYPE, 0,    C-TRANSPARENCY, -1, STD, 480, 265, 350, 190, 19, 7,     "Transparency:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Whether or not this product is transparent"
; AFR 5/4/09 - moved up
      COMBO, 15606,     0,     0, 1,  GLASS-TYPE, 0,      C-FRAME-TYPE, -1, STD, 480, 240, 350, 190, 19, 7,       "Frame Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, "The frame type for this fenestration product"
; AFR 5/4/09 - moved up
   CHECKBOX, 15607,     0,     0, 1,  GLASS-TYPE, 0,        C-DIVIDERS, -1, STD, 481, 265,  17, 150,     7,          "Dividers", RIGHT,                         "Check if fenestration product has dividers between panes"
; AFR 5/4/09 - moved up
   CHECKBOX, 15608,     0,     0, 1,  GLASS-TYPE, 0,   C-DIVIDED-LITES, -1, STD, 481, 290,  17, 150,     7,     "Divided Lites", RIGHT,                         "Check if fenestration product has true divided lites"

; AFR 6/24/09 - the following two controls have compliance flag = 6, display when compliance ruleset, and LEED
      COMBO, 15600,     0,     0, 1,  GLASS-TYPE, 0,   C-901-PROD-TYPE, -1, STD, 480, 115, 350, 190, 19, 6,     "Product Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, "ASHRAE fenestration product type"
      COMBO, 15606,     0,     0, 1,  GLASS-TYPE, 0,  C-901-FRAME-TYPE, -1, STD, 480, 140, 350, 190, 19, 6,       "Frame Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, "ASHRAE frame type for vertical fenestration"
      
   
    CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 1
       COMBO, 19179, 13131, 0, 1, GLASS-TYPE, 0, GLASS-TYPE-CODE,  0, STD, 165,  70, 250, 145, 19, 3, "Library Selection:",  LEFT, -135, 5, 0, LEFT, 4, 5, ""
       COMBO, 18306, 19019, 0, 1, GLASS-TYPE, 0, GLASS-PROP-CALC, -1, STD, 165,  95, 250, 145, 19, 3,  "Angular Data Use:", LEFT, -135, 5, 0, LEFT, 4, 5, "Method of modeling angular dependence of glass properties for Glass Types from the Library or imported from Window 5"
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;      STATIC,  1, GLASS-TYPE-CODE, 0, DESCRIPTION, -1, 0, 0, 30, 100, 250, STD, LEFT, "Desc: ",  "", 0, 3

; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;       LABEL, "Summary Glass Properties", STD, LEFT,  30, 138,  1, 0, 0, 310, 0, 3
;     NAVEDIT, 12062, 13142,   0, 1, 2504, GLASS-TYPE, 0, GLASS-TYPE-CODE, 0, GLASS-TYPE-CODE, 0,   NLAYER, -1, STD, 170, 195,  21,  40,  0, 3,       "Number of Panes:", LEFT, 20, 5, 0, LEFT, 4, 5, "Number of panes of glass in the window"
;     NAVEDIT, 12063, 13143, 759, 1, 2504, GLASS-TYPE, 0, GLASS-TYPE-CODE, 0, GLASS-TYPE-CODE, 0, U-CENTER, -1, STD, 170, 220,  21,  40,  2, 3,  "Center Glass U-Value:", LEFT, 20, 5, 0, LEFT, 4, 5, "The center of glass U-value of the selected glass type code"
;     NAVEDIT, 12156, 13132,   0, 1, 2504, GLASS-TYPE, 0, GLASS-TYPE-CODE, 0, GLASS-TYPE-CODE, 0,   SHDCOF,  0, STD, 170, 245,  21,  40,  3, 3,   "Shading Coefficient:", LEFT, 20, 5, 0, LEFT, 4, 5, "Solar transmittance defined for selected glass type code"
;     NAVEDIT, 12171, 13145,   0, 1, 2504, GLASS-TYPE, 0, GLASS-TYPE-CODE, 0, GLASS-TYPE-CODE, 0,     TSOL,  0, STD, 170, 270,  21,  40,  3, 3,   "Solar Trans (at 0°):", LEFT, 20, 5, 0, LEFT, 4, 5, "Solar transmittance defined for selected glass type code"
;     NAVEDIT, 12177, 13146,   0, 1, 2504, GLASS-TYPE, 0, GLASS-TYPE-CODE, 0, GLASS-TYPE-CODE, 0,     TVIS,  0, STD, 170, 295,  21,  40,  3, 3, "Visible Trans (at 0°):", LEFT, 20, 5, 0, LEFT, 4, 5, "Visible transmittance defined for selected glass type code"

; TO DO ?? - implement new graphic control - perhaps using JPGs?
;       LABEL, "Window Cross Section", STD, CENTER, 430, 10, 1, 0, 0, 0, 0, 3
;    METAFILE, 14398, 14398, 0, 1, GLASS-TYPE-CODE, 0, DRAWING, 0, 250, 66, 125, 160, 1, 1, 0

; TO DO ?? - implement new graphic control - perhaps using JPGs?
;       LABEL, "Window Appearance", STD, CENTER, 610, 10, 1, 0, 0, 0, 0, 3
;      BITMAP, 14392, 14392, 0, 1, GLASS-TYPE-CODE, 0, PICTURE, 0, 430, 66, 125, 160, 1, 1, 0

; TO DO - need to port the GRAPH control and migrate it to Olectra Chart
;       GRAPH, 29016, 29016, 0, 1, PowerDOE, 0, GraphGlass, -1, 240, 196, 160, 350, 1, 0
    ENDCASE
    
    CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 2
       LABEL, "Simplified Input Information", STD, LEFT,  30, 93,  1, 0, 0, 305, 0, 3
        EDIT, 13132, 13132,  759, 1, GLASS-TYPE, 0,     SHADING-COEF, -1, STD, 185, 115,  23,  60,  2, 3,     "Shading Coefficient:", LEFT, -140, 5, 1, LEFT, 4, 5, "Amount of solar radiation that the window transmits (relative to standard glass)"
        EDIT, 13133, 13133,    0, 1, GLASS-TYPE, 0,    GLASS-CONDUCT, -1, STD, 185, 140,  23,  60,  2, 3,       "Glass Conductance:", LEFT, -140, 5, 1, LEFT, 4, 5, "Amount of heat that the glass conducts (includes outside air film but not inside air film)"
        EDIT, 13134, 13146, 3006, 1, GLASS-TYPE, 0,        VIS-TRANS, -1, STD, 185, 165,  23,  60,  2, 3,   "Visible Transmittance:", LEFT, -140, 5, 1, LEFT, 4, 5, "Fraction of visible daylight that is transmitted through the glass (at normal incidence)"
        EDIT, 13135, 13135,    0, 1, GLASS-TYPE, 0,    OUTSIDE-EMISS, -1, STD, 185, 190,  23,  60,  2, 3,      "Outside Emissivity:", LEFT, -140, 5, 1, LEFT, 4, 5, "Infrared emissivity of the exterior finish of this window"
    ENDCASE

   ;******************************************
   ;  Component Tab
   ;******************************************
   TABPAGE, 3133,   760, 1, 3, NOTIMP, " Component Details "
   
    CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 1
       COMBO, 14387, 13131, 0, 1,      GLASS-TYPE,  0,   GLASS-TYPE-CODE,  0, STD, 145,  20, 250, 70, 19, 3, "Library Selection:",  LEFT, -115, 5, 0, LEFT, 4, 5, ""
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;      STATIC,  1, GLASS-TYPE-CODE, 0, DESCRIPTION, -1, 0, 0, 235,  25, 360, STD, LEFT, "Description: ",  "", 0, 3

       LABEL, "Glass Layers (Outside to Inside)", STD, LEFT, 30, 65, 1, 0, 0, 665, 0, 3
      SPREAD, 11515, 11515, 0, 1, 0, PowerDOE, 0, GlassSpread, 0, STD, 50, 85, 120, 615, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
     
       LABEL, "Gaps Between Glass Layers (Outside to Inside)", STD, LEFT, 30, 225, 1, 0, 0, 665, 0, 3
      SPREAD, 11519, 11519, 0, 1, 0, PowerDOE, 0, GlassGapSpread, 0, STD, 50, 245, 120, 615, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
    ENDCASE
    
    CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 2
      LABEL, "Component Details do not apply to the Simplified Specification Method", ITALIC, CENTER, 350, 80, 1, 0, 0, 0, 0, 3
    ENDCASE
   
   ;******************************************
   ;  Solar/Optical Details Tab
   ;******************************************
   TABPAGE, 3134,   760, 1, 3, NOTIMP, " Solar/Optical Details "
   
    CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 1
       COMBO, 14389, 13131, 0, 1,      GLASS-TYPE,  0,   GLASS-TYPE-CODE,  0, STD, 145,  20, 250, 70, 19, 3, "Library Selection:",  LEFT, -115, 5, 0, LEFT, 4, 5, ""
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;      STATIC,  1, GLASS-TYPE-CODE, 0, DESCRIPTION, -1, 0, 0, 235,  25, 360, STD, LEFT, "Description: ",  "", 0, 3

      SPREAD, 11521, 11521, 0, 1, 0, PowerDOE, 0, GTCSpread, 0, STD, 45, 70,  255, 609, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
      
        EDIT, 12907, 12907, 0, 1, GLASS-TYPE-CODE, 0, RBSOL-HEMI, -1, STD, 260, 332,  23,  60,  3, 3, "Solar Reflectance (from the inside):",   LEFT, -215, 5, 0, LEFT, 4, 5, ""
        EDIT, 12908, 12908, 0, 1, GLASS-TYPE-CODE, 0, RBVIS-HEMI, -1, STD, 595, 332,  23,  60,  3, 3, "Visible Reflectance (from the inside):", LEFT, -220, 5, 0, LEFT, 4, 5, ""
    ENDCASE
    
    CASE, GLASS-TYPE, 0, TYPE, -1, =, 1, 2
      LABEL, "Solar/Optical Details do not apply to the Simplified Specification Method", ITALIC, CENTER, 350, 80, 1, 0, 0, 0, 0, 3
    ENDCASE



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Window Layer Tabbed Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODTABDLG, 3087, 32012, 1,  50, 100, 360, 600, 0, "Window Layers Data", NOTIMP, 0, NOTIMP, 0 
 MODTABDLG, 3087, 32012, 1,  100, 100, 470, 710, 0, WINDOW-LAYER, "Window Layer Properties", NOTIMP, 0, NOTIMP, 0 
 
;   COMBO, 19074, 19074, 32092, 1, WINDOW-LAYER, 0, NAME,  0, STD, 300,  10, 260, 160, 21, "Currently Active Window Layer:", RIGHT, 290, 12, 0, LEFT, 355, 34, "Name of window layer; options allow renaming, deleting, copying, linking, save to library"
    COMBO, 19074, 19074, 32092, 1, WINDOW-LAYER, 0, NAME, -1, STD, 280, 15, 400, 200, 19, 3, "Currently Active Window Layer:", RIGHT, -10, 5, 0, LEFT, 4, 5, "List of all window layers defined in project; also allows library retrieval and creation"
    STATIC, 1, WINDOW-LAYER, 0, TYPE, 0, 0, 0, 510, 20, 175, STD, LEFT, "Type:  ",   "", 0, 3

   ;*****************************************
   ; Main Properties 
   ;*****************************************
   TABPAGE, 3088, 32092, 1, 3, NOTIMP, " Basic Specifications "
 
;   COMBO, 19074, 19074, 32092, 1, WINDOW-LAYER, 0,            NAME,  0, STD, 300,  10, 260, 160, 21, "Currently Active Window Layer:", RIGHT, 290, 12, 0, LEFT, 355, 34, "Name of window layer; options allow renaming, deleting, copying, linking, save to library"
;    LINE, 10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0

;  COMBO, 12321, 12321, 32092, 1, WINDOW-LAYER, 0,            NAME,  0, STD, 110,  60, 136, 200, 21, 3,       "Window Layer:",  LEFT,  20,  62, 0, LEFT, 205, 137, "List of all window layers defined in project; also allows library retrieval"

    EDIT, 12321, 12321, 32092, 1, WINDOW-LAYER, 0,            NAME,  0, STD, 155,  25,  23, 180, 32, 3,  "Window Layer Name:",  LEFT, -125, 5, 0, LEFT, 4, 5, "Name of window layer; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 12322, 12322, 32092, 1, WINDOW-LAYER, 0,            TYPE,  0, STD, 155,  50, 200, 180, 19, 3,  "Window Layer Type:",  LEFT, -125, 5, 0, LEFT, 4, 5, "Glass=plastic/transparent mat'l; Gap=air,argon,etc; Blind=slatted shade (e.g. venetian blind)"
    EDIT, 12323, 12323, 32092, 1, WINDOW-LAYER, 0,       THICKNESS,  0, STD, 155,  75,  23,  75,  6, 3,          "Thickness:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Thickness of the Layer"
    EDIT, 12324, 12324, 32092, 1, WINDOW-LAYER, 0,    CONDUCTIVITY,  0, STD, 155, 100,  23,  75,  6, 3,       "Conductivity:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Heat transfer rate through the layer, per degree "
      
    CASE,  WINDOW-LAYER,  0, TYPE,  -1,  =, 1, 1
      LABEL,     "Slat Data", STD, LEFT,  95, 158, 1, 0, 0, 335, 12328, 3
      COMBO, 12328, 12328, 32092, 1, WINDOW-LAYER, 0, SLAT-ORIENTATION,  0, STD, 245, 175,  85,  90, 19, 3,          "Slat Orientation:",  LEFT, -135, 5, 0, LEFT, 4, 5, "Whether the blinds are oriented in the X or Y plane of the window"
       EDIT, 12332, 12332, 32092, 1, WINDOW-LAYER, 0,       SLAT-WIDTH,  0, STD, 245, 200,  23,  60,  2, 3,                "Slat Width:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Width of the slat (in feet)"
       EDIT, 12330, 12330, 32092, 1, WINDOW-LAYER, 0,  SLAT-SEPARATION,  0, STD, 245, 225,  23,  60,  2, 3,           "Slat Separation:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Distance between slats (in feet)"
       EDIT, 12331, 12331, 32092, 1, WINDOW-LAYER, 0,       SLAT-ANGLE,  0, STD, 245, 250,  23,  60,  1, 3,                "Slat Angle:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Angle between slat and window's outward normal (e.g., horizontal slats in vertical window=0)"
       EDIT, 12333, 12333, 32092, 1, WINDOW-LAYER, 0,   SLAT-ANGLE-MIN,  0, STD, 245, 275,  23,  60,  1, 3,        "Minimum Slat Angle:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Minimum slat angle (for angle-adjustable slats) - limitation of the blind construction or controls"
       EDIT, 12334, 12334, 32092, 1, WINDOW-LAYER, 0,   SLAT-ANGLE-MAX,  0, STD, 245, 300,  23,  60,  1, 3,        "Maximum Slat Angle:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Maximum slat angle (for angle-adjustable slats) - limitation of the blind construction or controls"

      LABEL, "Infrared Data", STD, LEFT,  390,  108, 1, 0, 0, 645, 12325, 3
       EDIT, 12325, 12325, 32092, 1, WINDOW-LAYER, 0,         TRANS-IR,  0, STD, 565, 125,  23,  60,  3, 3,    "Infrared Transmittance:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Fraction of incident infrared radiation that the (glass or blind) layer transmits"
       EDIT, 12326, 12326, 32092, 1, WINDOW-LAYER, 0,          EMIS-IR,  0, STD, 565, 150,  23,  60,  3, 3, "Front Infrared Emissivity:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Hemispherical infrared emissivity of the front (or outside) of a glass or blind layer"
       EDIT, 12327, 12327, 32092, 1, WINDOW-LAYER, 0,      BACKEMIS-IR,  0, STD, 565, 175,  23,  60,  3, 3,  "Back Infrared Emissivity:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Hemispherical infrared emissivity of the back (or inside) of a glass or blind layer"
       
      LABEL,    "Blind Data", STD, LEFT,  390,  233, 1, 0, 0, 645, 12335, 3
       EDIT, 12335, 12335, 32092, 1, WINDOW-LAYER, 0,      BLIND-COVER,  0, STD, 565, 250,  23,  60,  2, 3,            "Blind Coverage:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Fraction of the window area covered by the blind"
       EDIT, 12336, 12336, 32092, 1, WINDOW-LAYER, 0,  BLIND-COVER-MIN,  0, STD, 565, 275,  23,  60,  2, 3,    "Minimum Blind Coverage:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Minimum fraction of (glazed) window area covered by movable blinds"
       EDIT, 12337, 12337, 32092, 1, WINDOW-LAYER, 0,  BLIND-COVER-MAX,  0, STD, 565, 300,  23,  60,  2, 3,    "Maximum Blind Coverage:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Maximum fraction of (glazed) window area covered by movable blinds"
    ENDCASE    

    CASE,  WINDOW-LAYER,  0, TYPE,  -1,  =, 1, 2
      LABEL, "Infrared Data", STD, LEFT, 390,  108, 1, 0, 0, 645, 12338, 3
       EDIT, 12338, 12325, 32092, 1, WINDOW-LAYER, 0,         TRANS-IR,  0, STD, 565, 125,  23,  60,  3, 3,    "Infrared Transmittance:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Fraction of incident infrared radiation that the (glass or blind) layer transmits"
       EDIT, 12339, 12326, 32092, 1, WINDOW-LAYER, 0,          EMIS-IR,  0, STD, 565, 150,  23,  60,  3, 3, "Front Infrared Emissivity:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Hemispherical infrared emissivity of the front (or outside) of a glass or blind layer"
       EDIT, 12340, 12327, 32092, 1, WINDOW-LAYER, 0,      BACKEMIS-IR,  0, STD, 565, 175,  23,  60,  3, 3,  "Back Infrared Emissivity:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Hemispherical infrared emissivity of the back (or inside) of a glass or blind layer"
    ENDCASE    

    CASE,  WINDOW-LAYER,  0, TYPE,  -1,  =, 1, 3
       EDIT, 12341, 12341, 32092, 1, WINDOW-LAYER, 0,   D-CONDUCTIVITY,  0, STD, 290, 175,  23,  90,  7, 3,   "Temperature Derivative of Conductivity:",  LEFT, -260, 5, 1, LEFT, 4, 5, "The (constant) change in Conductivity per change in temperature"
       EDIT, 12342, 12342, 32092, 1, WINDOW-LAYER, 0,        VISCOSITY,  0, STD, 290, 200,  23,  90,  7, 3,                                "Viscosity:",  LEFT, -260, 5, 1, LEFT, 4, 5, "Viscosity of the gas in the gap"
       EDIT, 12343, 12343, 32092, 1, WINDOW-LAYER, 0,      D-VISCOSITY,  0, STD, 290, 225,  23,  90,  7, 3,      "Temperature Derivative of Viscosity:",  LEFT, -260, 5, 1, LEFT, 4, 5, "The (constant) change in gas Viscosity per change in temperature"
       EDIT, 12344, 12344, 32092, 1, WINDOW-LAYER, 0,          DENSITY,  0, STD, 290, 250,  23,  90,  7, 3,                                  "Density:",  LEFT, -260, 5, 1, LEFT, 4, 5, "Density of the gas in the gap"
       EDIT, 12345, 12345, 32092, 1, WINDOW-LAYER, 0,        D-DENSITY,  0, STD, 290, 275,  23,  90,  7, 3,        "Temperature Derivative of Density:",  LEFT, -260, 5, 1, LEFT, 4, 5, "The (constant) change in gas Density per change in temperature"
       EDIT, 12348, 12348, 32092, 1, WINDOW-LAYER, 0,     PRANDTL-NUMB,  0, STD, 290, 300,  23,  90,  7, 3,                           "Prandtl Number:",  LEFT, -260, 5, 1, LEFT, 4, 5, "Prandtl number of the gas in the gap (default is for Argon)"
       EDIT, 12347, 12347, 32092, 1, WINDOW-LAYER, 0,   D-PRANDTL-NUMB,  0, STD, 290, 325,  23,  90,  7, 3, "Temperature Derivative of Prandtl Number:",  LEFT, -260, 5, 1, LEFT, 4, 5, "The (constant) change in Prandtl Number per change in temperatures"
    ENDCASE    
    
   ;*****************************************
   ; Transmittances & Reflectance 
   ;*****************************************
   TABPAGE, 3089, 32092, 1, 3, NOTIMP, " Transmittances and Reflectance "
 
;   COMBO, 19075, 19074, 32092, 1, WINDOW-LAYER, 0, NAME,  0, STD, 300,  10, 260, 160, 21, "Currently Active Window Layer:", RIGHT, 290, 12, 0, LEFT, 355, 34, "Name of window layer; options allow renaming, deleting, copying, linking, save to library"
;    LINE, 10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0

    CASE,  WINDOW-LAYER,  0, TYPE,  -1,  =, 1, 1
      LABEL,     "Solar Transmittances & Reflectances", STD, LEFT,  20,  58, 1, 0, 0, 315, 12349, 3
       EDIT, 12349, 12349, 32092, 1, WINDOW-LAYER, 0,     TRANS-SOL-BB,  0, STD, 255,  75,  23,  60,  3, 3,       "Beam-Beam Solar Transmittance:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Fraction of incident beam solar that is transmitted as beam radiation (at normal incidence)"
       EDIT, 12350, 12350, 32092, 1, WINDOW-LAYER, 0,      REFL-SOL-BB,  0, STD, 255, 100,  23,  60,  3, 3,   "Front Beam-Beam Solar Reflectance:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Fraction of beam solar incident on front that is reflected as beam (at normal incidence)"
       EDIT, 12351, 12351, 32092, 1, WINDOW-LAYER, 0,  BACKREFL-SOL-BB,  0, STD, 255, 125,  23,  60,  3, 3,    "Back Beam-Beam Solar Reflectance:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Fraction of beam solar, incident on back side, that is reflected as beam (at normal incidence)"
       EDIT, 12352, 12352, 32092, 1, WINDOW-LAYER, 0,     TRANS-SOL-BH,  0, STD, 255, 150,  23,  60,  3, 3,         "Beam-Hemi Solar Reflectance:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Fraction of incident beam solar that is reflected as diffuse radiation (at normal incidence)"
       EDIT, 12353, 12353, 32092, 1, WINDOW-LAYER, 0,      REFL-SOL-BH,  0, STD, 255, 175,  23,  60,  3, 3,   "Front Beam-Hemi Solar Reflectance:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Fraction of beam solar incident on front that is reflected as diffuse (at normal incidence)"
       EDIT, 12354, 12354, 32092, 1, WINDOW-LAYER, 0,  BACKREFL-SOL-BH,  0, STD, 255, 200,  23,  60,  3, 3,    "Back Beam-Hemi Solar Reflectance:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Fraction of beam solar, incident on back side, that is reflected as diffuse (at normal incidence)"
       EDIT, 12355, 12355, 32092, 1, WINDOW-LAYER, 0,     TRANS-SOL-HH,  0, STD, 255, 225,  23,  60,  3, 3,         "Hemi-Hemi Solar Reflectance:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Fraction of incident diffuse solar that is reflected"
       EDIT, 12356, 12356, 32092, 1, WINDOW-LAYER, 0,      REFL-SOL-HH,  0, STD, 255, 250,  23,  60,  3, 3,   "Front Hemi-Hemi Solar Reflectance:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Fraction of diffuse solar incident on front that is reflected"
       EDIT, 12357, 12357, 32092, 1, WINDOW-LAYER, 0,  BACKREFL-SOL-HH,  0, STD, 255, 275,  23,  60,  3, 3,    "Back Hemi-Hemi Solar Reflectance:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Fraction of diffuse solar, incident on back side, that is reflected"
   
      LABEL,     "Visible Transmittances & Reflectances", STD, LEFT,  365,  58, 1, 0, 0, 670, 12363, 3
       EDIT, 12363, 12363, 32092, 1, WINDOW-LAYER, 0,     TRANS-VIS-BB,  0, STD, 610,  75,  23,  60,  3, 3,     "Beam-Beam Visible Transmittance:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Fraction of incident visible beam solar that is transmitted as beam (at normal incidence)"
       EDIT, 12364, 12364, 32092, 1, WINDOW-LAYER, 0,      REFL-VIS-BB,  0, STD, 610, 100,  23,  60,  3, 3, "Front Beam-Beam Visible Reflectance:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Fraction of incident visible beam solar that is reflected as beam (at normal incidence)"
       EDIT, 12365, 12365, 32092, 1, WINDOW-LAYER, 0,  BACKREFL-VIS-BB,  0, STD, 610, 125,  23,  60,  3, 3,  "Back Beam-Beam Visible Reflectance:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Fraction of visible beam solar, incident on back side, that is reflected (at normal incidence)"
       EDIT, 12366, 12366, 32092, 1, WINDOW-LAYER, 0,     TRANS-VIS-BH,  0, STD, 610, 150,  23,  60,  3, 3,       "Beam-Hemi Visible Reflectance:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Fraction of incident visible beam solar that is transmitted as diffuse (at normal incidence)"
       EDIT, 12367, 12367, 32092, 1, WINDOW-LAYER, 0,      REFL-VIS-BH,  0, STD, 610, 175,  23,  60,  3, 3, "Front Beam-Hemi Visible Reflectance:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Fraction of incident visible beam solar that is reflected as diffuse (at normal incidence)"
       EDIT, 12368, 12368, 32092, 1, WINDOW-LAYER, 0,  BACKREFL-VIS-BH,  0, STD, 610, 200,  23,  60,  3, 3,  "Back Beam-Hemi Visible Reflectance:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Fraction of visible beam solar, incident on back side, reflected as diffuse (at normal incidence)"
       EDIT, 12372, 12372, 32092, 1, WINDOW-LAYER, 0,     TRANS-VIS-HH,  0, STD, 610, 225,  23,  60,  3, 3,       "Hemi-Hemi Visible Reflectance:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Fraction of incident visible diffuse solar that is reflected"
       EDIT, 12370, 12370, 32092, 1, WINDOW-LAYER, 0,      REFL-VIS-HH,  0, STD, 610, 250,  23,  60,  3, 3, "Front Hemi-Hemi Visible Reflectance:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Fraction of incident visible diffuse solar that is reflected"
       EDIT, 12371, 12371, 32092, 1, WINDOW-LAYER, 0,  BACKREFL-VIS-HH,  0, STD, 610, 275,  23,  60,  3, 3,  "Back Hemi-Hemi Visible Reflectance:",  LEFT, -230, 5, 0, LEFT, 4, 5, "Fraction of visible diffuse solar, incident on back side, that is reflected"
      LABEL, "Note:  Hemi is an abbreviation for Hemispherical.", ITALIC, LEFT,  20, 330, 1, 0, 0, 0, 0, 3
    ENDCASE    

    CASE,  WINDOW-LAYER,  0, TYPE,  -1,  =, 1, 2
      LABEL,     "Solar Transmittances & Reflectances", STD, LEFT,  20,  58, 1, 0, 0, 315, 12373, 3
       EDIT, 12373, 12349, 32092, 1, WINDOW-LAYER, 0,     TRANS-SOL-BB,  0, STD, 255,  75,  23,  60,  3, 3,       "Beam-Beam Solar Transmittance:",  LEFT, -220, 5, 1, LEFT, 4, 5, "Fraction of incident beam solar that is transmitted as beam radiation (at normal incidence)"
       EDIT, 12376, 12350, 32092, 1, WINDOW-LAYER, 0,      REFL-SOL-BB,  0, STD, 255, 100,  23,  60,  3, 3,   "Front Beam-Beam Solar Reflectance:",  LEFT, -220, 5, 1, LEFT, 4, 5, "Fraction of beam solar incident on front that is reflected as beam (at normal incidence)"
       EDIT, 12375, 12351, 32092, 1, WINDOW-LAYER, 0,  BACKREFL-SOL-BB,  0, STD, 255, 125,  23,  60,  3, 3,    "Back Beam-Beam Solar Reflectance:",  LEFT, -220, 5, 1, LEFT, 4, 5, "Fraction of beam solar, incident on back side, that is reflected as beam (at normal incidence)"
    ENDCASE    

    CASE,  WINDOW-LAYER,  0, TYPE,  -1,  =, 1, 3
      LABEL, "Note:  No transmittance or reflectance data necessary for gap layers.", ITALIC, CENTER, 350, 100, 1, 0, 0, 0, 0, 3
    ENDCASE    



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Lighting System / Luminaire / Lamp Tabbed Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

 MODTABDLG, 3166, 3166, 1, 30, 30, 470, 710, 0, NOTIMP, "Lighting System, Luminaire and Lamp Type Properties", NOTIMP, 0, NOTIMP, 0

   ;******************************************
   ;  Lighting System Dialog Page
   ;******************************************
;   MODDLG, 2532, 32084, 1, 100, 100, 470, 620, 0, "Lighting System Data", NOTIMP, 0, NOTIMP, 0 
   TABPAGE, 3167, 32084, 1, 3, LIGHTING-SYSTEM, " Lighting System "

     COMBO, 19033, 19033, 32084, 1, LIGHTING-SYSTEM, 0, NAME,  0, STD, 240,   5, 400, 250, 19, 3, "Currently Active Lighting System:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all lighting systems defined in project; also allows library retrieval and creation"
     STATIC, 1, LIGHTING-SYSTEM, 0, LTG-CALC-METHOD, 0, 0, 0, 510, 10, 175, STD, LEFT, "Method: ",   "", 0, 3

      LINE,  20, 40, 685, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

      EDIT,   13584, 13584, 32084, 1, LIGHTING-SYSTEM,  0,            NAME, -1, STD, 130,  55,  23, 200, 32, 3,     "Lighting System:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Name of lighting system; right mouse quick menu options allow deleting, copying, linking and saving to library"
     COMBO,   12308, 12308, 32084, 1, LIGHTING-SYSTEM,  0, LTG-CALC-METHOD, -1, STD, 175,  85, 100, 155, 19, 3,  "Calculation Method:",  LEFT, -145, 5, 0, LEFT, 4, 5, "Whether you are using a Luminaire Type or gross power consumption for lighting calculations"

      EDIT,   14528, 14528, 32084, 1, LIGHTING-SYSTEM,  0,     DESCRIPTION, -1, STD, 425,  55,  23, 250, 64, 3,             "Descrip:", RIGHT,   -8, 5, 0, LEFT, 4, 5, "A description of the Lighting System"      

    CASE, LIGHTING-SYSTEM,  0, LTG-CALC-METHOD,  -1, =, 1, 0
       LABEL, "Luminaire", STD, LEFT,  30, 153, 1, 0, 0, 330, 19039, 3
       COMBO, 19039, 19039, 32084, 1, LIGHTING-SYSTEM, 0,   LUMINAIRE-TYPE, -1, STD, 150, 175, 250, 180, 19, 3,      "Luminaire Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Name of luminaire in the llighting system; includes lamps and ballasts"   
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;       STATIC, 1, LIGHTING-SYSTEM, 0, LUMINAIRE-TYPE, -1, 1, LUMINAIRE-TYPE, 0,      DESCRIPTION, 64,  50, 200, 280, STD, LEFT,           "Description: ",   "", 0, 3
;       STATIC, 1, LIGHTING-SYSTEM, 0, LUMINAIRE-TYPE, -1, 1, LUMINAIRE-TYPE, 0,      NO-OF-LAMPS,  0,  50, 220,  -1, STD, LEFT,       "Number of Lamps:   ", "", 0, 3
;       STATIC, 1, LIGHTING-SYSTEM, 0, LUMINAIRE-TYPE, -1, 1, LUMINAIRE-TYPE, 0, ACCEPT-LAMP-SIZE,  0,  50, 240,  -1, STD, LEFT,     "Accepts Lamp Size:   ", "", 0, 3
;       STATIC, 1, LIGHTING-SYSTEM, 0, LUMINAIRE-TYPE, -1, 1, LUMINAIRE-TYPE, 0,    ACCEPT-CONFIG,  0,  50, 260,  -1, STD, LEFT, "Accepts Configuration:  ",  "", 0, 3
       COMBO, 13583, 13583, 32084, 1, LIGHTING-SYSTEM, 0, LUMINAIRE-CONFIG, -1, STD, 150, 280, 200, 180, 19, 3,       "Configuration:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Used to calculate thermal effects that influence lamp input power and light output"      
       
       LABEL, "Ballast", STD, LEFT, 375, 93, 1, 0, 0, 675, 19047, 3
       COMBO, 19047, 19047, 32084, 1, LIGHTING-SYSTEM,  0,    BALLAST-TYPE, -1, STD, 495, 115, 250, 180, 19, 3,        "Ballast Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Type of ballast" 
       
       LABEL, "Lamps", STD, LEFT, 375, 153, 1, 0, 0, 675, 19042, 3
       COMBO, 19042, 19042, 32084, 1, LIGHTING-SYSTEM,  0,       LAMP-TYPE, -1, STD, 495, 175, 250, 180, 19, 3,           "Lamp Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Name of the lamp type in the lighting system; form the library or custom built"  
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;       STATIC, 1, LIGHTING-SYSTEM, 0,       LAMP-TYPE, -1, 1,  LAMP-TYPE, 0,     DESCRIPTION, 64, 315, 200, 270, STD, LEFT,         "Description: ",   "", 0, 3
;       STATIC, 1, LIGHTING-SYSTEM, 0,       LAMP-TYPE, -1, 1,  LAMP-TYPE, 0,            SIZE,  0, 315, 220,  -1, STD, LEFT,                "Size:   ", "", 0, 3
;       STATIC, 1, LIGHTING-SYSTEM, 0,       LAMP-TYPE, -1, 1,  LAMP-TYPE, 0,  INIT-LUMEN-OUT,  0, 315, 240,  -1, STD, LEFT,  "Rated Light Output:   ", "", 0, 3
;       STATIC, 1, LIGHTING-SYSTEM, 0,       LAMP-TYPE, -1, 1,  LAMP-TYPE, 0,     POWER-INPUT,  2, 315, 260,  -1, STD, LEFT,         "Rated Power:   ", "", 0, 3
;       STATIC, 1,          NOTIMP, 0,          NOTIMP, -1, 0,                                  0, 315, 280,  -1, STD, LEFT,            "Efficacy:   ", "", 0, 3
;       STATIC, 1, LIGHTING-SYSTEM, 0,       LAMP-TYPE, -1, 1,  LAMP-TYPE, 0,    LUMEN-DEPREC,  2, 315, 300,  -1, STD, LEFT,  "Lumen Depreciation:   ", "", 0, 3

       
; TO DO ?? - via STATICs => must incorporate secondary com/key retrieval
;       LABEL, "Luminaire Coefficients of Utilization", STD, LEFT, 30, 320, 1, 0, 0, 500, 0, 3
;
;       LABEL,   "Room", STD, RIGHT, 60, 322, 1, 0, 0, 3
;       LABEL, "Cavity", STD, RIGHT, 60, 338, 1, 0, 0, 3
;       LABEL,  "Ratio", STD, RIGHT, 60, 354, 1, 0, 0, 3
;       LABEL,      "1", STD, RIGHT, 57, 375, 1, 0, 0, 3
;       LABEL,      "5", STD, RIGHT, 57, 395, 1, 0, 0, 3
;       LABEL,     "10", STD, RIGHT, 57, 415, 1, 0, 0, 3
;   
;       LABEL, "Ceiling Cavity Reflectance", STD, CENTER, 258, 305, 1, 0, 0, 3
;       LABEL,                       "0.80", STD, CENTER, 129, 321, 1, 0, 0, 3
;       LABEL,                       "0.50", STD, CENTER, 258, 321, 1, 0, 0, 3
;       LABEL,                       "0.30", STD, CENTER, 387, 321, 1, 0, 0, 3
;      
;       LABEL,           "Wall Reflectance", STD, CENTER, 258, 338, 1, 0, 0, 3
;       LABEL,                       "0.50", STD, CENTER,  87, 354, 1, 0, 0, 3
;       LABEL,                       "0.30", STD, CENTER, 129, 354, 1, 0, 0, 3
;       LABEL,                       "0.10", STD, CENTER, 171, 354, 1, 0, 0, 3
;       LABEL,                       "0.50", STD, CENTER, 216, 354, 1, 0, 0, 3
;       LABEL,                       "0.30", STD, CENTER, 258, 354, 1, 0, 0, 3
;       LABEL,                       "0.10", STD, CENTER, 300, 354, 1, 0, 0, 3
;       LABEL,                       "0.50", STD, CENTER, 345, 354, 1, 0, 0, 3
;       LABEL,                       "0.30", STD, CENTER, 387, 354, 1, 0, 0, 3
;       LABEL,                       "0.10", STD, CENTER, 429, 354, 1, 0, 0, 3
;      
;       LINE,  20, 370, 452, 370, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;       LINE,  65, 337, 452, 337, 1,   DOT, 0, 0, 0, NONE, 1, 0, 0, 3
;
;       LINE,  65, 320,  65, 430, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;       LINE, 194, 320, 194, 430, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;       LINE, 323, 320, 323, 430, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;       LINE, 452, 320, 452, 430, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;
; - MUST REVISE THESE STATICS TO UTILIZE ENHANCED SECONDARY COM/KEY RETRIEVAL WHICH INCLUDES SECONDARY ARRAY INDEX
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-1, 8, 0, 2,  87, 375, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-1, 7, 0, 2, 129, 375, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-1, 6, 0, 2, 171, 375, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-1, 5, 0, 2, 216, 375, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-1, 4, 0, 2, 258, 375, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-1, 3, 0, 2, 300, 375, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-1, 2, 0, 2, 345, 375, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-1, 1, 0, 2, 387, 375, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-1, 0, 0, 2, 429, 375, -1, STD, CENTER, "", "", 0   
;
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-5, 8, 0, 2,  87, 395, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-5, 7, 0, 2, 129, 395, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-5, 6, 0, 2, 171, 395, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-5, 5, 0, 2, 216, 395, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-5, 4, 0, 2, 258, 395, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-5, 3, 0, 2, 300, 395, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-5, 2, 0, 2, 345, 395, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-5, 1, 0, 2, 387, 395, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE,  0, CU-RCR-5, 0, 0, 2, 429, 395, -1, STD, CENTER, "", "", 0   
;
;       STATIC, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 8, 0, 2,  87, 415, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 7, 0, 2, 129, 415, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 6, 0, 2, 171, 415, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 5, 0, 2, 216, 415, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 4, 0, 2, 258, 415, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 3, 0, 2, 300, 415, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 2, 0, 2, 345, 415, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 1, 0, 2, 387, 415, -1, STD, CENTER, "", "", 0   
;       STATIC, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 0, 0, 2, 429, 415, -1, STD, CENTER, "", "", 0   
    ENDCASE

    CASE, LIGHTING-SYSTEM,  0, LTG-CALC-METHOD,  -1, =, 1, 1
       EDIT,  12311, 12311, 32084, 1, LIGHTING-SYSTEM,  0,  TOT-POWER-INPUT, -1, STD, 175, 125,  23, 70,  1, 3,          "Total Power Input:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Total electrical input power for the Lighting System at full power (also called 'active power')"
       EDIT,  12314, 12314, 32084, 1, LIGHTING-SYSTEM,  0,     COEF-OF-UTIL, -1, STD, 175, 150,  23, 70,  3, 3, "Coefficient of Utilization:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Fraction of light output from lamp/luminaire combination that reaches the Workplane Height"
       EDIT,  12316, 12316, 32084, 1, LIGHTING-SYSTEM,  0,  TOT-LAMP-LUMENS, -1, STD, 175, 175,  23, 70,  1, 3,          "Total Lamp Lumens:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Total number of lumens produced by all lamps in the lighting subsystem (at 70% of lamp life)"
    ENDCASE

   ;******************************************
   ;  Luminaire Dialog Page
   ;******************************************
;   MODDLG, 2530, 10248, 1, 100, 100, 470, 620, 0, "Luminaire Data", NOTIMP, 0, NOTIMP, 0 
   TABPAGE, 3168, 10248, 1, 3, LUMINAIRE-TYPE, " Luminaire Type "

     COMBO, 19032, 19032, 0, 1, LUMINAIRE-TYPE, 0, NAME,  0, STD, 240,   5, 400, 250, 19, 3, "Currently Active Luminaire Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all luminaire types defined in project; also allows library retrieval and creation"

      LINE,  20, 40, 685, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 13537, 13537, 0, 1, LUMINAIRE-TYPE, 0,             NAME, -1, STD, 130,  55,  23, 200, 32, 3,                "Luminaire Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Name of luminaire type; right mouse quick menu options allow deleting, copying, linking and saving to library"
     EDIT, 13538, 13538, 0, 1, LUMINAIRE-TYPE, 0,      DESCRIPTION, -1, STD, 130,  85,  23, 400, 64, 3,                   "Description:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Description of the Type of Luminaire (the 'luminaire' includes all lamps and ballasts)"
     EDIT, 13539, 13539, 0, 1, LUMINAIRE-TYPE, 0,      NO-OF-LAMPS, -1, STD, 250, 115,  23,  54,  0, 3, "Number of Lamps per Luminaire:",  LEFT, -220, 5, 0, LEFT, 4, 5, "Number of lamps in the luminaire (the 'luminaire' includes all lamps and ballasts)"
    COMBO, 13540, 13540, 0, 1, LUMINAIRE-TYPE, 0, ACCEPT-LAMP-SIZE, -1, STD, 180, 140, 250, 140, 19, 3,             "Accepts Lamp Size:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Use to avoid inappropriate lamps in the luminaire (with inaccurate Coefficients Of Utilization)"
    COMBO, 13542, 13542, 0, 1, LUMINAIRE-TYPE, 0,    LUM-MAINT-CAT, -1, STD, 180, 165, 250, 140, 19, 3,          "Maintenance Category:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Used to calculate decrease in light output due to dirt accumulation"
    COMBO, 13543, 13543, 0, 1, LUMINAIRE-TYPE, 0,  OPERATING-ATMOS, -1, STD, 180, 190, 250, 140, 19, 3,          "Operating Atmosphere:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Used to calculate decrease in light output due to dirt accumulation"
    
     EDIT, 13544, 13544, 0, 1, LUMINAIRE-TYPE, 0,   CLEANING-CYCLE, -1, STD, 250, 215,  23,  54,  2, 3,          "Cleaning Cycle (yrs):",  LEFT, -220, 5, 0, LEFT, 4, 5, "Used to calculate decrease in light output due to dirt accumulation"
    COMBO, 13541, 13541, 0, 1, LUMINAIRE-TYPE, 0,    ACCEPT-CONFIG,  0, STD, 180, 240, 200, 140, 19, 3,         "Accepts Configuration:",  LEFT, -150, 5, 0, LEFT, 4, 5, "The Lighting subsystem can have any one of these three Luminaire Configurations"    
    COMBO, 12242, 13541, 0, 1, LUMINAIRE-TYPE, 0,    ACCEPT-CONFIG,  1, STD, 335, 240, 200, 140, 19, 3,                               "",  LEFT, -150, 5, 0, LEFT, 4, 5, "The Lighting subsystem can have any one of these three Luminaire Configurations"    
    COMBO, 12243, 13541, 0, 1, LUMINAIRE-TYPE, 0,    ACCEPT-CONFIG,  2, STD, 490, 240, 200, 140, 19, 3,                               "",  LEFT, -150, 5, 0, LEFT, 4, 5, "The Lighting subsystem can have any one of these three Luminaire Configurations"    
  
    LABEL, "Coefficients of Utilization", STD, LEFT, 30, 277, 1, 0, 0, 675, 0, 3

    LABEL,   "Room", STD, RIGHT,  85, 299, 1, 0, 0, 0, 0, 3
    LABEL, "Cavity", STD, RIGHT,  85, 314, 1, 0, 0, 0, 0, 3
    LABEL,  "Ratio", STD, RIGHT,  85, 329, 1, 0, 0, 0, 0, 3
    LABEL,      "1", STD, RIGHT,  82, 354, 1, 0, 0, 0, 0, 3
    LABEL,      "5", STD, RIGHT,  82, 379, 1, 0, 0, 0, 0, 3
    LABEL,     "10", STD, RIGHT,  82, 404, 1, 0, 0, 0, 0, 3
   
    LABEL,                       "0.80", STD, CENTER, 165, 306, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.50", STD, CENTER, 315, 306, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.30", STD, CENTER, 465, 306, 1, 0, 0, 0, 0, 3
    LABEL, "Ceiling Cavity Reflectance", STD,   LEFT, 545, 306, 1, 0, 0, 0, 0, 3

    LABEL,                       "0.50", STD, CENTER, 117, 328, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.30", STD, CENTER, 165, 328, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.10", STD, CENTER, 213, 328, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.50", STD, CENTER, 267, 328, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.30", STD, CENTER, 315, 328, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.10", STD, CENTER, 373, 328, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.50", STD, CENTER, 417, 328, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.30", STD, CENTER, 465, 328, 1, 0, 0, 0, 0, 3
    LABEL,                       "0.10", STD, CENTER, 513, 328, 1, 0, 0, 0, 0, 3
    LABEL,           "Wall Reflectance", STD,   LEFT, 545, 328, 1, 0, 0, 0, 0, 3
   
    LINE,  45, 345, 645, 345, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
    LINE,  90, 323, 645, 323, 1,   DOT, 0, 0, 0, NONE, 1, 0, 0, 3

    LINE,  90, 300,  90, 425, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
    LINE, 240, 305, 240, 425, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
    LINE, 390, 305, 390, 425, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
    LINE, 540, 305, 540, 425, 1, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3

    EDIT,  13546, 13546, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-1, 8, STD,  97, 350,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"      
    EDIT,  13547, 13546, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-1, 7, STD, 145, 350,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"      
    EDIT,  13548, 13546, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-1, 6, STD, 193, 350,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"      
    EDIT,  13549, 13546, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-1, 5, STD, 247, 350,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13550, 13546, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-1, 4, STD, 295, 350,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13551, 13546, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-1, 3, STD, 343, 350,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13552, 13546, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-1, 2, STD, 397, 350,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13553, 13546, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-1, 1, STD, 445, 350,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13554, 13546, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-1, 0, STD, 493, 350,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"

    EDIT,  13555, 13555, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-5, 8, STD,  97, 375,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13556, 13555, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-5, 7, STD, 145, 375,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13557, 13555, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-5, 6, STD, 193, 375,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13558, 13555, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-5, 5, STD, 247, 375,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13559, 13555, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-5, 4, STD, 295, 375,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13560, 13555, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-5, 3, STD, 343, 375,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13561, 13555, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-5, 2, STD, 397, 375,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13562, 13555, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-5, 1, STD, 445, 375,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13563, 13555, 0, 1, LUMINAIRE-TYPE, 0,  CU-RCR-5, 0, STD, 493, 375,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"

    EDIT,  13564, 13564, 0, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 8, STD,  97, 400,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13565, 13564, 0, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 7, STD, 145, 400,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13566, 13564, 0, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 6, STD, 193, 400,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13567, 13564, 0, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 5, STD, 247, 400,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13568, 13564, 0, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 4, STD, 295, 400,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13569, 13564, 0, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 3, STD, 343, 400,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13570, 13564, 0, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 2, STD, 397, 400,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13571, 13564, 0, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 1, STD, 445, 400,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"
    EDIT,  13572, 13564, 0, 1, LUMINAIRE-TYPE, 0, CU-RCR-10, 0, STD, 493, 400,  23, 40, 2, 3, "", RIGHT, -2, 5, 0, LEFT, 4, 5, "Fraction of the lamp/luminaire light output that reaches the Workplane Height"

; TO DO ?? - implement new graphic control - perhaps using JPGs?
;    BITMAP, 12759, 12759, 0, 1, LUMINAIRE-TYPE, 0, DRAWING, 0, 315, 100, 120, 120, 1, 1, 114
;    BITMAP, 12760, 12760, 0, 1, LUMINAIRE-TYPE, 0, PICTURE, 0, 465, 100, 120, 120, 1, 1, 120

   ;******************************************
   ;  Lamp Type Dialog Page
   ;******************************************
;   MODDLG, 2533, 32084, 1, 100, 100, 325, 500, 0, "Lamp Data", NOTIMP, 0, NOTIMP, 0 
   TABPAGE, 3169, 32084, 1, 3, LAMP-TYPE, " Lamp Type "

    COMBO, 19050, 19050, 0, 1, LAMP-TYPE, 0,             NAME,  0, STD, 240,   5, 400, 210, 19, 3, "Currently Active Lamp Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all lamp types defined in project; also allows library retrieval and creation"
     STATIC, 1, LAMP-TYPE, 0, CATEGORY, 0, 0, 0, 470, 10, 215, STD, LEFT, "Category: ",   "", 0, 3

      LINE,  20, 40, 685, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 12295, 12295, 0, 1, LAMP-TYPE, 0,           NAME, -1, STD, 110,  55,  23, 200, 32, 3,          "Lamp Type:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Name of lamp type; options allow renaming, deleting, copying, linking, save to library"        
     EDIT, 14529, 14529, 0, 1, LAMP-TYPE, 0,    DESCRIPTION, -1, STD, 110,  80,  23, 400, 64, 3,        "Description:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Description of the lamp type"

    COMBO, 13182, 13182, 0, 1, LAMP-TYPE, 0,       CATEGORY, -1, STD, 110, 105, 300, 160, 19, 3,           "Category:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "The type of Lamp"
    COMBO, 13183, 13183, 0, 1, LAMP-TYPE, 0,           SIZE, -1, STD, 110, 130, 300, 160, 19, 3,               "Size:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Must match Luminaire's Accepts Lamp Size; forces compatible luminaire/lamp combinations"
     EDIT, 12296, 12296, 0, 1, LAMP-TYPE, 0, INIT-LUMEN-OUT, -1, STD, 170, 155,  23,  83,  2, 3, "Rated Light Output:",  LEFT, -140, 5, 1, LEFT, 4, 5, "Lamp's light output; after seasoning the lamp for 100 hours"   
     EDIT, 12297,  1000, 0, 1, LAMP-TYPE, 0,    POWER-INPUT, -1, STD, 170, 180,  23,  83,  2, 3,        "Rated Power:",  LEFT, -140, 5, 1, LEFT, 4, 5, "Nominal lamp power consumption"
     EDIT, 12298,  1001, 0, 1, LAMP-TYPE, 0,   LUMEN-DEPREC, -1, STD, 170, 205,  23,  83,  2, 3, "Lumen Depreciation:",  LEFT, -140, 5, 1, LEFT, 4, 5, "Ratio of the lamp's light output at 70% of its rated life to its initial light output"

;    STATIC, 1, NOTIMP, 0, NOTIMP, -1, 0, 0, 15, 178, -1, STD, LEFT,              "Efficacy:   ", "", 0, 3

;    BITMAP, 12317, 12317, 0, 1, LAMP-TYPE, 0,        PICTURE, 0, 350, 75, 120, 120, 1, 1, 120



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     ZONE - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
   
; MODTABDLG, 3042, 10031, 1,  50, 100, 350, 600, 0, "Air-Side HVAC Zone Parameters", NOTIMP, 0, NOTIMP, 0
; MODTABDLG, 3042, 10031, 1, 30, 30, 470, 710, 0, ZONE, "Air-Side HVAC Zone Parameters", NOTIMP, 0, NOTIMP, 0
; AFR 8/13/09 - changed height from 470 to 555 to accomodate compliance keywords at the bottom of the dialog.
 MODTABDLG, 3042, 10031, 1, 30, 30, 575, 800, 0, ZONE, "Air-Side HVAC Zone Parameters", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 19182, 19182, 0, 1, ZONE, 0, NAME, 0, STD, 210,  15, 400, 250, 19, 3, "Currently Active Zone:", LEFT, -140, 5, 0, LEFT, 4, 5, "List of all zones defined in project; also allows library retrieval and creation"
   STATIC, 1, ZONE, 0, TYPE, 0, 0, 0, 485, 20, 250, STD, LEFT, "Zone Type:  ",   "", 0, 3

    ;*****************************************
    ; Zone Mode
    ;*****************************************
    TABPAGE, 3043, 29035, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 14605, 14605,   0, 1, ZONE, 0, NAME,             -1, STD, 155,  10,  23, 200, 32, 3,    "Thermal Zone Name:",  LEFT, -135, 5, 0, LEFT, 4, 5, "Name of zone; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 14606, 12018,   0, 1, ZONE, 0, SPACE,            -1, STD, 155,  35, 350, 200, 19, 3,  "Corresponding Space:",  LEFT, -135, 5, 0, LEFT, 4, 5, "Name of the space that comprises this thermal zone (must be 1 to 1 correlation)"
      COMBO, 15624, 15624,   0, 1, ZONE, 0, PARENT,           -1, STD, 155,  60, 350, 200, 19, 3,   "Parent HVAC System:",  LEFT, -135, 5, 0, LEFT, 4, 5, "Name of the space that comprises this thermal zone (must be 1 to 1 correlation)"
      COMBO, 14607, 12263,   0, 1, ZONE, 0, TYPE,             -1, STD, 155,  85, 120, 120, 19, 3,            "Zone Type:",  LEFT, -105, 5, 0, LEFT, 4, 5, "Whether the zone is Conditioned, Unconditioned, or a Plenum"
;      COMBO, 14614, 12250,   0, 1, ZONE, 0, SIZING-OPTION,    -1, STD, 155, 110, 100, 120, 19, 3,        "Sizing Option:",  LEFT, -105, 5, 0, LEFT, 4, 5, "Method of sizing equipment & air flow rates;Adjust loads=more detailed calculation"   ; SAC 11/24/10 - removed

      LABEL, "Thermostat", STD, LEFT, 35, 140, 1, 0, 0, 275, 14612, 3
      COMBO, 14612, 60003,   0, 1, ZONE, 0, THERMOSTAT-TYPE,  -1, STD, 155, 160, 100, 120, 19, 3,                 "Type:",  LEFT, -105, 5, 0, LEFT, 4, 5, "2-Position=on/off; Proportional=capacity is linear f(DT); Reverse Action=for VAV's"
      EDIT,  14613, 60004,   0, 1, ZONE, 0, THROTTLING-RANGE, -1, STD, 155, 185,  23,  60,  1, 3,       "Throttle Range:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Degrees that room temp must go thru for heat/cool output to go from zero to the maximum"
; SAC 11/30/10 - added
      COMBO, 19235, 19235,   0, 1, ZONE, 0, THERMOSTAT-LOCN,  -1, STD, 155, 210, 150, 120, 19, 3,             "Location:",  LEFT, -105, 5, 0, LEFT, 4, 5, "Specifies whether the zone thermostat is within the zone, or in the return airflow"
; SAC 10/23/00 - Compliance keyword
   CHECKBOX, 15485,     0,   0, 1, ZONE, 0,  C-HTG-SETBACK,   -1, STD,  85, 237,  17, 195,     7,  "Heating Setback (compliance)", RIGHT,                 "Checked if zone thermostat has heating setback capability"

; JJH 2/15/2004 change zone multiplier to static to force input in shell module
;     EDIT,  14610, 12245, 769, 1, ZONE, 0, FLOOR-MULTIPLIER, -1, STD, 570,  35,  23,  60,  1, 3,     "Floor Multiplier:",  LEFT, -120, 5, 1, LEFT, 4, 5, "The number of floors in the facility that are identical, and served by the same HVAC system"
;     EDIT,  14611, 12245, 769, 1, ZONE, 0, MULTIPLIER,       -1, STD, 570,  60,  23,  60,  1, 3,           "Multiplier:",  LEFT, -120, 5, 1, LEFT, 4, 5, "The number of zones in the facility identical to this one, and served by the same HVAC system"
      LABEL, "Floor Multiplier:", STD, LEFT , 450, 35,  1, 0, 0,   0, 0, 3
      LABEL, "Space Multiplier:", STD, LEFT , 450, 60,  1, 0, 0,   0, 0, 3
      STATIC, 1, ZONE ,  0, FLOOR-MULTIPLIER, -1, 0, 1, 625,  35, -1, STD, RIGHT, "", "", 0, 3
      STATIC, 1, ZONE ,  0, MULTIPLIER,       -1, 0, 1, 625,  60, -1, STD, RIGHT, "", "", 0, 3
      COMBO, 14608, 60005,   0, 1, ZONE, 0, ZONE-REPORTS,     -1, STD, 570,  85,  90,  60, 19, 3,         "Zone Reports:",  LEFT, -120, 5, 0, LEFT, 4, 5, "Whether or not DOE-2 includes summary reports for this zone in the output reports"

      LABEL, "Zone Design Flow Rates", STD, LEFT, 430, 140, 1, 0, 0, 675, 14615, 3
      EDIT,  14615, 12247,   0, 1, ZONE, 0, FLOW/AREA,        -1, STD, 570, 160,  23,  60,  2, 3,      "Min Design Flow:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Minimum design supply air flow rate for the zone (standard cfm per unit zone floor area)"
      EDIT,  14616, 12248,   0, 1, ZONE, 0, OA-FLOW/PER,      -1, STD, 570, 185,  23,  60,  1, 3,       "OA Flow/Person:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Minimum flow rate of outside air (standard cfm) per zone occupant, at peak occupancy"
      EDIT,  14617, 12249,   0, 1, ZONE, 0, MIN-FLOW-RATIO,   -1, STD, 570, 210,  23,  60,  2, 3,   "Minimum Flow Ratio:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Minimum allowable supply air flow rate (as a fraction of the design flow rate)"


      LABEL, "Zone Cooling and Heating", STD, LEFT,    35, 268, 1, 0, 0, 675,     0, 3
      LABEL, "Thermostat Schedules",     STD, CENTER, 205, 294, 1, 0, 0,   0,     0, 3
      LABEL, "Indoor Design",            STD, CENTER, 345, 281, 1, 0, 0,   0,     0, 3
      LABEL, "Temperature",              STD, CENTER, 345, 294, 1, 0, 0,   0,     0, 3
      LABEL, "Total",                    STD, CENTER, 432, 281, 1, 0, 0,   0,     0, 3
      LABEL, "Capacity",                 STD, CENTER, 432, 294, 1, 0, 0,   0,     0, 3
      LABEL, "Sensible",                 STD, CENTER, 532, 281, 1, 0, 0,   0, 14654, 3
      LABEL, "Capacity",                 STD, CENTER, 532, 294, 1, 0, 0,   0, 14654, 3
      LABEL, "Reheat",                   STD, CENTER, 632, 281, 1, 0, 0,   0, 14655, 3
      LABEL, "Delta T",                  STD, CENTER, 632, 294, 1, 0, 0,   0, 14655, 3

      COMBO, 14648, 12178,   0, 1, ZONE, 0, COOL-TEMP-SCH,    -1, STD, 115, 325, 200, 185, 19, 3,              "Cooling:",  LEFT, -60, 5, 0, LEFT,     4,   5, "A schedule that specifies the setpoint of the zone cooling thermostat"
      EDIT,  14650, 12251,   0, 1, ZONE, 0, DESIGN-COOL-T,    -1, STD, 315, 325,  23,  60,  1, 3,                      "",  LEFT,   0, 5, 1, CENTER, -30, -16, "Desired space T, used to calculate supply airflow rate required for peak zonal cooling loads"
      EDIT,  14652, 13050,   0, 1, ZONE, 0, COOLING-CAPACITY, -1, STD, 390, 325,  23,  85,  0, 3,                      "",  LEFT,   0, 5, 1, CENTER, -43, -16, "Total zonal cooling capacity (at ARI conditions) of the chilled water or DX cooling coil"
;      EDIT,  14654, 13052,   0, 1, ZONE, 0, COOL-SH-CAP,      -1, STD, 490, 325,  23,  85,  0, 3,                      "",  LEFT,   0, 5, 1, CENTER, -43, -16, "Sensible heat removal capacity of the zone's air cooling device at ARI rated conditions"   ; SAC 11/24/10 - removed

      COMBO, 14649, 12181,   0, 1, ZONE, 0, HEAT-TEMP-SCH,    -1, STD, 115, 350, 200, 185, 19, 3,              "Heating:",  LEFT, -60, 5, 0, LEFT,     4,   5, "A schedule that specifies the setpoint of the zone heating thermostat"
      EDIT,  14651, 12252,   0, 1, ZONE, 0, DESIGN-HEAT-T,    -1, STD, 315, 350,  23,  60,  1, 3,                      "",  LEFT,   0, 5, 0, CENTER,   4,   5, "Desired space T, used to calculate supply airflow rate required for peak zonal heating loads"
      EDIT,  14653, 13051,   0, 1, ZONE, 0, HEATING-CAPACITY, -1, STD, 390, 350,  23,  85,  0, 3,                      "",  LEFT,   0, 5, 0, CENTER,   4,   5, "Heating capacity (at ARI conditions) of the zonal heating HVAC system"
      EDIT,  14655, 13026,   0, 1, ZONE, 0, REHEAT-DELTA-T,   -1, STD, 590, 350,  23,  85,  1, 3,                      "",  LEFT,   0, 5, 1, CENTER, -43, -41, "Maximum increase in supply air temperature due to zonal reheat coils"

; AFR 8/13/09 - added
      LABEL, "Compliance Settings (references)", STD, LEFT, 35, 390, 1, 0, 0, 675, 0, 6
      LABEL, "Conditioning:",           STD, LEFT,   44, 410, 1, 0, 0,   0, 0, 6
      LABEL, "Schedule Type:",          STD, LEFT,   44, 430, 1, 0, 0,   0, 0, 6
      LABEL, "Heating Source:",         STD, LEFT,   44, 450, 1, 0, 0,   0, 0, 6
      LABEL, "System Type Exception:",  STD, LEFT,  384, 410, 1, 0, 0,   0, 0, 6
      LABEL, "Economizer Exception:",   STD, LEFT,  384, 430, 1, 0, 0,   0, 0, 6
      LABEL, "ERV Exception:",          STD, LEFT,  384, 450, 1, 0, 0,   0, 0, 6

   ; SAC 11/9/09 - added max lengths to prevent statics from overwriting labels (above)
      STATIC, 1, ZONE, 0, C-901-CONDITION,  0, 0, 0, 295, 410, 150, STD, RIGHT, "",  "", 0, 6
      STATIC, 1, ZONE, 0, C-901-SCH-TYPE,   0, 0, 0, 295, 430, 150, STD, RIGHT, "",  "", 0, 6
      STATIC, 1, ZONE, 0, C-HTG-SYS-CLASS,  0, 0, 0, 295, 450, 150, STD, RIGHT, "",  "", 0, 6
      STATIC, 1, ZONE, 0, C-SYS-EXCEPTION1, 0, 0, 0, 675, 410, 140, STD, RIGHT, "",  "", 0, 6
      STATIC, 1, ZONE, 0, C-SYS-EXCEPTION2, 0, 0, 0, 675, 430, 140, STD, RIGHT, "",  "", 0, 6
      STATIC, 1, ZONE, 0, C-SYS-EXCEPTION3, 0, 0, 0, 675, 450, 140, STD, RIGHT, "",  "", 0, 6

    
    ;*****************************************
    ; Air Flow Mode
    ;*****************************************
    TABPAGE, 3044, 29035, 1, 3, NOTIMP, " Air Flow "
;      LINE,  10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;      COMBO, 19183, 19182, 0, 1, ZONE, 0, NAME,       -1, STD, 260,  10, 200, 200, 21, 3, "Currently Active Zone:", RIGHT, 250,  13, 0, LEFT, 4, 5, "List of all zones defined in project; also allows library retrieval and creation"

      LABEL, "Design Flow",           STD,   CENTER, 113,   5, 1, 0, 0, 0, 0, 3
      LABEL, "Design",                STD,   CENTER, 190,   5, 1, 0, 0, 0, 0, 3
      LABEL, "Min Design Flow",       STD,   CENTER, 285,   5, 1, 0, 0, 0, 0, 3
      LABEL, "Minimum Flow",          STD,   CENTER, 410,   5, 1, 0, 0, 0, 0, 3
      LABEL, "Max Flow",              STD,   CENTER, 510,   5, 1, 0, 0, 0, 0, 3

      LABEL, "Overall",               STD,   LEFT,    20,  45, 1, 0, 0, 0, 0, 3
      LABEL, "Cooling",               STD,   LEFT,    20,  70, 1, 0, 0, 0, 0, 3
      LABEL, "Heating",               STD,   LEFT,    20,  95, 1, 0, 0, 0, 0, 3

      LABEL, "AC/h",                  SMALL, CENTER, 315,  24, 1, 0, 0, 0, 0, 3
      LABEL, "Minimum Flow Schedule", STD,   CENTER, 645,  24, 1, 0, 0, 0, 0, 3

      EDIT,  14657, 12257, 0, 1, ZONE, 0, ASSIGNED-FLOW,    -1, STD,  75,  40,  23,  75,  0, 3, "",  LEFT,  15, 5, 1, CENTER, -37, -16, ""
      EDIT,  14656, 12247, 0, 1, ZONE, 0, FLOW/AREA,        -1, STD, 230,  40,  23,  50,  2, 3, "",  LEFT,  15, 5, 1, CENTER, -25, -16, "Minimum design supply air flow rate for the zone (standard cfm per unit zone floor area)"
      EDIT,  14658, 12259, 0, 1, ZONE, 0, AIR-CHANGES/HR,   -1, STD, 290,  40,  23,  50,  2, 3, "",  LEFT,  15, 5, 0, CENTER, -25, -16, "Design cooling supply air flow rate (number of times air in the zone is replaced in an hour)"
      EDIT,  14659, 13015, 0, 1, ZONE, 0, MIN-FLOW/AREA,    -1, STD, 355,  40,  23,  50,  2, 3, "",  LEFT,  15, 5, 1, CENTER, -25, -16, "Minimum total supply air flow rate per square foot of floor area (alternative to Min Flow Ratio)"
      EDIT,  14660, 12249, 0, 1, ZONE, 0, MIN-FLOW-RATIO,   -1, STD, 415,  40,  23,  55,  3, 3, "",  LEFT,  15, 5, 1, CENTER, -28, -16, "Minimum allowable supply air flow rate (as a fraction of the design flow rate)"
      COMBO, 14661, 60000, 0, 1, ZONE, 0, MIN-FLOW-SCH,     -1, STD, 550,  40, 200, 200, 19, 3, "",  LEFT,  10, 5, 0, CENTER,   4,   5, "Schedule minimum allowable total supply air flow rate per square foot of floor area"

      EDIT,  19242, 19242, 0, 1, ZONE, 0, COOL-SUP/RET-DT,  -1, STD, 165,  65,  23,  50,  2, 3, "",  LEFT,  15, 5, 1, CENTER, -25, -41, "The design cooling differential between the zonal supply and return temperatures for airflow sizing"
      EDIT,  14662, 12261, 0, 1, ZONE, 0, CMIN-FLOW/AREA,   -1, STD, 355,  65,  23,  50,  2, 3, "",  LEFT,  15, 5, 0, CENTER,   4,   5, "Minimum allowable cooling supply air flow rate per square foot of floor area"
      EDIT,  14663, 13041, 0, 1, ZONE, 0, CMIN-FLOW-RATIO,  -1, STD, 415,  65,  23,  50,  3, 3, "",  LEFT,  15, 5, 0, CENTER,   4,   5, "The min airflow ratio of the cold duct damper controller at the inlet of the mixing box"
      COMBO, 14664, 63000, 0, 1, ZONE, 0, CMIN-FLOW-SCH,    -1, STD, 550,  65, 200, 200, 19, 3, "",  LEFT,  10, 5, 0, CENTER,   4,   5, "Scheduled Cooling Min Flow Ratio of the cold duct damper at the inlet of the mixing box"

      EDIT,  14666, 12258, 0, 1, ZONE, 0, HASSIGNED-FLOW,   -1, STD,  75,  90,  23,  75,  0, 3, "",  LEFT,  15, 5, 0, CENTER,   4,   5, ""
      EDIT,  19243, 19243, 0, 1, ZONE, 0, HEAT-SUP/RET-DT,  -1, STD, 165,  90,  23,  50,  2, 3, "",  LEFT,  15, 5, 0, CENTER,   4,   5, "The design heating differential between the zonal supply and return temperatures for airflow sizing"
      EDIT,  14665, 12256, 0, 1, ZONE, 0, HFLOW/AREA,       -1, STD, 230,  90,  23,  50,  2, 3, "",  LEFT,  15, 5, 0, CENTER,   4,   5, "Minimum design heating zonal supply air flow rate (standard cfm per unit floor area)"
      EDIT,  14667, 12260, 0, 1, ZONE, 0, HAIR-CHANGES/HR,  -1, STD, 290,  90,  23,  50,  2, 3, "",  LEFT,  15, 5, 0, CENTER,   4,   5, "Design heating supply air flow rate (number of times air in the zone is replaced in an hour)"
      EDIT,  14668, 12262, 0, 1, ZONE, 0, HMIN-FLOW/AREA,   -1, STD, 355,  90,  23,  50,  2, 3, "",  LEFT,  15, 5, 0, CENTER,   4,   5, "Minimum allowable heating supply air flow rate per square foot of floor area"
      EDIT,  14669, 13027, 0, 1, ZONE, 0, HMIN-FLOW-RATIO,  -1, STD, 415,  90,  23,  55,  3, 3, "",  LEFT,  15, 5, 0, CENTER,   4,   5, "Minimum airflow ratio of the hot duct damper controller at the inlet of the mixing box (VAV only)"
      EDIT,  19200, 19200, 0, 1, ZONE, 0, HMAX-FLOW-RATIO,  -1, STD, 485,  90,  23,  50,  2, 3, "",  LEFT,  15, 5, 1, CENTER, -25, -66, "For a reverse-action VAV terminal, specifies the ratio of the maximum heating airflow to the cooling airflow"    ; SAC 12/11/09
      COMBO, 14670, 60010, 0, 1, ZONE, 0, HMIN-FLOW-SCH,    -1, STD, 550,  90, 200, 200, 19, 3, "",  LEFT,  10, 5, 0, CENTER,   4,   5, "Scheduled Cooling Min Flow Ratio of the hot duct damper at the inlet of the mixing box"

      COMBO, 14671, 13017, 0, 1, ZONE, 0, MIN-FLOW-SOURCE,  -1, STD, 550, 120, 110, 200, 19, 3, "Minimum Flow Source:", LEFT, -137,  5, 0, LEFT, 4, 5, "Source of makeup air when the supply airflow falls below the Minimum Flow Ratio"
      COMBO, 14671, 13017, 0, 1, ZONE, 0, MIN-FLOW-CTRL     -1, STD, 550, 145, 110, 200, 19, 3,"Minimum Flow Control:", LEFT, -137,  5, 0, LEFT, 4, 5, "Reset of zone VAV box minimum flow due to Demand Control Ventilation hourly minimum OA needs"
      EDIT,  19237, 19237, 0, 1, ZONE, 0, BYPASS-FLOW-RATI, -1, STD, 550, 170,  23,  60,  2, 3,   "Bypass Flow Ratio:", LEFT, -137,  5, 1, LEFT, 4, 5, "For a terminal that bypasses unneeded flow, specifies the flow ratio at which bypass starts"

      LABEL, "Zone Terminal and Fans", STD, LEFT, 20, 224, 1, 0, 0, 770, 14672, 3

      COMBO, 14672, 13013, 0, 1, ZONE, 0, TERMINAL-TYPE,    -1, STD, 130, 245, 300, 160, 19, 3,      "Terminal Type:", LEFT, -100, 5, 0, LEFT, 4, 5, "(PIU) VAV=VAV or CV reheat; Series=primary & 2nd air; Parallel=2nd air only"
; SAC 11/30/10 - restored (& revised) commented out controls & added more...
      COMBO, 14674, 13055, 0, 1, ZONE, 0, MASTER-ZONE,      -1, STD, 130, 270, 200, 160, 19, 3,        "Master Zone:", LEFT, -100, 5, 0, LEFT, 4, 5, "The master zone that supplies air to this subzone"
      COMBO, 19236, 19236, 0, 1, ZONE, 0, RETURN-PLENUM,    -1, STD, 130, 295, 200, 160, 19, 3,      "Return Plenum:", LEFT, -100, 5, 0, LEFT, 4, 5, "When multiple plenums exist in the system, the plenum to which this zone returns air"

      EDIT,  14675, 13056, 0, 1, ZONE, 0, ZONE-FAN-RATIO,   -1, STD, 400, 245,  23,  70,  3, 3,          "Fan Ratio:", LEFT,  -70, 5, 1, LEFT, 4, 5, "Zone air flow rate, expressed as a fraction of the primary supply  air flow rate"
      EDIT,  14676, 60001, 0, 1, ZONE, 0, ZONE-FAN-FLOW,    -1, STD, 400, 270,  23,  70,  3, 3,           "Fan Flow:", LEFT,  -70, 5, 1, LEFT, 4, 5, "The capacity of the fan in the terminal box of a Powered Induction Unit(PIU) system"
      EDIT,  14677, 60002, 0, 1, ZONE, 0, ZONE-FAN-KW/FLOW, -1, STD, 400, 295,  23,  70,  6, 3,          "Fan Power:", LEFT,  -70, 5, 1, LEFT, 4, 5, "Power consumption of the fan in the terminal box of a PIU system (kW per cfm)"

; SAC 11/30/10 - added third column
      COMBO, 19238, 19238, 0, 1, ZONE, 0, ZONE-FAN-RUN,     -1, STD, 640, 245, 250, 130, 19, 3,         "Fan Enable:", LEFT,  -85, 5, 0, LEFT, 4, 5, "Specifies the thermostat control band in which the fan in a fan-powered terminal operates"
      COMBO, 19239, 19239, 0, 1, ZONE, 0, ZONE-FAN-CTRL,    -1, STD, 640, 270, 250, 130, 19, 3,        "Volume Ctrl:", LEFT,  -85, 5, 0, LEFT, 4, 5, "PIU fan may be constant-volume or variable-volume"
      COMBO, 19240, 19240, 0, 1, ZONE, 0, ZONE-FAN-KW-FPLR, -1, STD, 640, 295, 300, 130, 19, 3,       "Power f(PLR):", LEFT,  -85, 5, 0, LEFT, 4, 5, "Curve that modifies the PIU fan's electric input ratio as a function of part load ratio"
      COMBO, 14673, 13054, 0, 1, ZONE, 0, INDUCED-AIR-SRC,  -1, STD, 640, 320, 250, 130, 19, 3,      "Induction Src:", LEFT,  -95, 5, 0, LEFT, 4, 5, "The source of induced air for a fan-powered terminal"
      EDIT,  19241, 19241, 0, 1, ZONE, 0, INDUCTION-RATIO,  -1, STD, 640, 345,  23,  70,  2, 3,    "Induction Ratio:", LEFT,  -95, 5, 1, LEFT, 4, 5, "For Terminal Induction Unit, the ratio of induced airflow to primary airflow"

; SAC 11/30/10 - added diffuser controls
      LABEL, "Diffuser Efficiency and UFAD/DV Heat Plumes", STD, LEFT, 20, 380, 1, 0, 0, 360, 19244, 3
      LABEL, "Cooling",                STD,   CENTER, 158, 399, 1, 0, 0, 0, 19244, 3
      LABEL, "Heating",                STD,   CENTER, 228, 399, 1, 0, 0, 0, 19245, 3
      LABEL, "Deadband",               STD,   CENTER, 298, 399, 1, 0, 0, 0, 19246, 3

      EDIT,  19244, 19244, 0, 1, ZONE, 0, DIFFUSER-LOSS-CL, -1, STD, 130, 415,  23,  55,  2, 3,  "Diffuser Loss:", LEFT,  -90, 5, 0, LEFT, 4, 5, "Fraction of cooling supply air that bypasses directly into the return air"
      EDIT,  19245, 19245, 0, 1, ZONE, 0, DIFFUSER-LOSS-HT, -1, STD, 200, 415,  23,  55,  2, 3,                "", LEFT,   -1, 5, 0, LEFT, 4, 5, "Fraction of heating supply air that bypasses directly into the return air"
      EDIT,  19246, 19246, 0, 1, ZONE, 0, DIFFUSER-LOSS-DB, -1, STD, 270, 415,  23,  55,  2, 3,                "", LEFT,   -1, 5, 1, LEFT, 4, 5, "Fraction of deadband supply air that bypasses directly into the return air"

      EDIT,  19247, 19247, 0, 1, ZONE, 0, PLUME-COOL,       -1, STD, 130, 440,  23,  55,  2, 3,          "Plume:", LEFT,  -90, 5, 0, LEFT, 4, 5, "Fraction of cooling heat gain that bypasses directly into the return air"
      EDIT,  19248, 19248, 0, 1, ZONE, 0, PLUME-HEAT,       -1, STD, 200, 440,  23,  55,  2, 3,                "", LEFT,   -1, 5, 0, LEFT, 4, 5, "Fraction of heating heat gain that bypasses directly into the return air"
      EDIT,  19249, 19249, 0, 1, ZONE, 0, PLUME-DEADBAND,   -1, STD, 270, 440,  23,  55,  2, 3,                "", LEFT,   -1, 5, 1, LEFT, 4, 5, "Fraction of deadband heat gain that bypasses directly into the return air"


    ;*****************************************
    ; Outdoor Air Mode
    ;*****************************************
    TABPAGE, 3045, 29035, 1, 3, NOTIMP, " Outdoor Air "
;      LINE,  10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;      COMBO, 19184, 19182, 0, 1, ZONE, 0, NAME,       -1, STD, 260,  10, 200, 200, 19, 3, "Currently Active Zone:", RIGHT, 250, 5, 0, LEFT, 4, 5, "List of all zones defined in project; also allows library retrieval and creation"

      LABEL, "Outdoor Air", STD, LEFT,  60,  22, 1, 0, 0, 270, 0, 3
      EDIT,  14678, 13018, 0, 1, ZONE, 0, OUTSIDE-AIR-FLOW,   0, STD, 185,  45,  23,  60,  0, 3,                "Air Flow:", LEFT, -110, 5, 1, LEFT, 4, 5, "Minimum zonal outside air flow rate (in standard cfm); this method takes precedence"
      EDIT,  14679, 12248, 0, 1, ZONE, 0, OA-FLOW/PER,        0, STD, 185,  70,  23,  60,  1, 3,         "Flow per Person:", LEFT, -110, 5, 1, LEFT, 4, 5, "Minimum flow rate of outside air (standard cfm) per zone occupant, at peak occupancy"
      EDIT,  14680, 13020, 0, 1, ZONE, 0, OA-CHANGES,         0, STD, 185,  95,  23,  60,  2, 3,             "Air Changes:", LEFT, -110, 5, 1, LEFT, 4, 5, "Minimum zonal outside air flow rate (# of times per hour total volume of air is replaced)"
; SAC 12/19/05 - Added access to OA-FLOW/AREA
      EDIT,  17893,     0, 0, 1, ZONE, 0, OA-FLOW/AREA,       0, STD, 185, 120,  23,  60,  2, 3,           "Flow per Area:", LEFT, -110, 5, 1, LEFT, 4, 5, "Minimum flow rate of outside air (standard cfm) per unit of zone area"

      LABEL, "Exhaust Air", STD, LEFT, 355,  22, 1, 0, 0, 640, 0, 3
; SDG 11/28/06 - Added new keyword AIRFLOW-TRACKING
     COMBO, 18317,     0, 0, 1,  ZONE, 0, AIRFLOW-TRACKING,   0, STD, 455,  45, 180, 135, 19, 3,            "Tracking Ctrl", LEFT,  -85, 5, 0, LEFT, 4, 5, "Coordinates the tracking of the exhaust airflow with the supply"
      EDIT,  14681, 13021, 0, 1, ZONE, 0, EXHAUST-FLOW,       0, STD, 520,  70,  23,  70,  1, 3,                    "Flow:", LEFT, -150, 5, 1, LEFT, 4, 5, "Flow rate of air that is directly exhausted from the zone (in standard cfm)"
      EDIT,  14682, 13022, 0, 1, ZONE, 0, EXHAUST-KW/FLOW,    0, STD, 490,  95,  23, 100,  6, 3,             "kW per Flow:", LEFT, -120, 5, 1, LEFT, 4, 5, "Electrical energy consumption of the zonal exhaust fan (per standard cfm of exhaust air)"
      EDIT,  14683, 13023, 0, 1, ZONE, 0, EXHAUST-STATIC,     0, STD, 520, 120,  23,  70,  2, 3,         "Static Pressure:", LEFT, -150, 5, 1, LEFT, 4, 5, "Total pressure produced by the zonal exhaust fan (in inches of water)"
      EDIT,  14684, 13024, 0, 1, ZONE, 0, EXHAUST-EFF,        0, STD, 520, 145,  23,  70,  2, 3,  "Efficiency (mech+elec):", LEFT, -150, 5, 1, LEFT, 4, 5, "The combined efficiency of the zonal exhaust fan and motor (at design conditions)"
; SDG 11/28/06 - Added new keywords EXHAUST-FAN-CTRL, EXHAUST-EIR-FPLR, EXHAUST-FAN-SCH, AIRFLOW-TRACKING
     COMBO, 18314,     0, 0, 1,  ZONE, 0, EXHAUST-FAN-CTRL,   0, STD, 455, 170, 180, 135, 19, 3,                 "Control:", LEFT,  -85, 5, 0, LEFT, 4, 5, "May be either constant volume or variable-flow"
     COMBO, 18315,     0, 0, 1,  ZONE, 0, EXHAUST-EIR-FPLR,   0, STD, 455, 195, 180, 135, 19, 3,             "Power fFlow:", LEFT,  -85, 5, 0, LEFT, 4, 5, "Curve Fit: Power as a function of the fan's flow ratio"
; SAC 1/27/09 - Added new keyword EXHAUST-SOURCE
     COMBO, 18980,     0, 0, 1,  ZONE, 0, EXHAUST-SOURCE,     0, STD, 455, 220, 180, 135, 19, 3,                  "Source:", LEFT,  -85, 5, 0, LEFT, 4, 5, "Specifies the source of the make up air required by the exhaust fan"
     COMBO, 18316,     0, 0, 1,  ZONE, 0, EXHAUST-FAN-SCH,    0, STD, 455, 245, 180, 135, 19, 3,              "Flow Sched:", LEFT,  -85, 5, 0, LEFT, 4, 5, "If runs fewer hours than system fan, or if variable-flow"

; SAC 10/23/00 - Compliance keyword
; SAC 1/27/09 - re-positioned to squeeze in another exhaust control above
; DEM 10/26/12 - added new keywords for T24 efficiency lookup
      LABEL, "Exhaust Fan (compliance)", STD, LEFT, 55, 307, 1, 0, 0, 730, 15482, 7
       EDIT, 19333,     0, 0, 1, ZONE, 0, C-XFAN-QTY,         0, STD, 200, 330,  23,  70,  2, 7,           "Number of Fans:", LEFT, -130, 5, 1, LEFT, 4, 5, "The number of exhaust fans serving the zone"
       EDIT, 15482,     0, 0, 1, ZONE, 0, C-EXH-FAN-BHP,      0, STD, 200, 355,  23,  70,  2, 7,           "Total Brake HP:", LEFT, -130, 5, 1, LEFT, 4, 5, "The total brake horsepower of exhaust fans serving the zone"
       EDIT, 15488,     0, 0, 1, ZONE, 0, C-EXH-FAN-NOM-HP,   0, STD, 200, 380,  23,  70,  2, 7,         "Total Nominal HP:", LEFT, -130, 5, 1, LEFT, 4, 5, "The total nameplate horsepower of exhaust fans serving the zone"
       EDIT, 15483,     0, 0, 1, ZONE, 0, C-EF-DRIVE-EFF,     0, STD, 200, 405,  23,  70,  2, 7,        "Drive Efficiency:", LEFT, -130, 5, 1, LEFT, 4, 5, "The average drive efficiency of exhaust fans serving the zone"
       EDIT, 15484,     0, 0, 1, ZONE, 0, C-EF-MOTOR-EFF,     0, STD, 200, 430,  23,  70,  2, 7,        "Motor Efficiency:", LEFT, -130, 5, 1, LEFT, 4, 5, "The average motor efficiency of exhaust fans serving the zone"
         COMBO, 19334, 0, 0, 1, ZONE, 0,    C-XFAN-MTR-TYPE, 0, STD, 480, 330, 300, 200, 19, 7,     "Motor Effic. Category:", LEFT, -130, 5, 0, LEFT, 4, 5, "The category describing the exhaust fan motor efficiency"
         COMBO, 19335, 0, 0, 1, ZONE, 0, C-XFAN-MTR-SNC-SPD, 0, STD, 480, 355, 300,  90, 19, 7,     "Motor Synch Speed:", LEFT, -130, 5, 0, LEFT, 4, 5, "The synchronous speed of the exhaust fan motor"
         COMBO, 19336, 0, 0, 1, ZONE, 0,    C-XFAN-MTR-ENCL, 0, STD, 480, 380, 300,  90, 19, 7,     "Motor Enclosure:", LEFT, -130, 5, 0, LEFT, 4, 5, "The type of enclosure for the exhaust fan motor"
         COMBO, 19337, 0, 0, 1, ZONE, 0,    C-XFAN-MOTOR-SUB,  0, STD, 480, 405, 300, 170, 19, 7,     "Motor Subtype:", LEFT, -130, 5, 0, LEFT, 4, 5, "Motor phase and subtype classification"

    
    ;*****************************************
    ; Cooling Mode
    ;*****************************************
    TABPAGE, 3046, 29035, 1, 3, NOTIMP, " Cooling "
;      LINE,  10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;      COMBO, 19185, 19182, 0, 1, ZONE, 0, NAME,       -1, STD, 260,  10, 200, 200, 19, 3, "Currently Active Zone:", RIGHT, 250, 5, 0, LEFT, 4, 5, "List of all zones defined in project; also allows library retrieval and creation"

      LABEL, "Cooling Design Parameters", STD, LEFT,  30,  23, 1, 0, 0, 680, 0, 3
      EDIT,  14685, 12251, 0, 1, ZONE, 0, DESIGN-COOL-T,     -1, STD, 250,  45,  23,  60,  1, 3, "Cooling Design Temperature:", LEFT, -205, 5, 1, LEFT, 4, 5, "Desired space T, used to calculate supply airflow rate required for peak zonal cooling loads"
      EDIT,  14686, 13050, 0, 1, ZONE, 0, COOLING-CAPACITY,  -1, STD, 220,  70,  23,  90,  0, 3, "Cooling Capacity:",           LEFT, -175, 5, 1, LEFT, 4, 5, "Total zonal cooling capacity (at ARI conditions) of the chilled water or DX cooling coil"
;      EDIT,  14687, 13052, 0, 1, ZONE, 0, COOL-SH-CAP,       -1, STD, 220,  95,  23,  90,  0, 3, "Cooling Sensible Heat Cap:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Sensible heat removal capacity of the zone's air cooling device at ARI rated conditions"   ; SAC 11/24/10 - removed
      EDIT,  14688, 13045, 0, 1, ZONE, 0, MAX-COOL-RATE,     -1, STD, 220,  95,  23,  90,  0, 3, "Maximum Cooling Rate:",       LEFT, -175, 5, 1, LEFT, 4, 5, "Maximum net cooling rate for the zone (limits DOE-2's sizing calculation)"
      COMBO, 14689, 12178, 0, 1, ZONE, 0, COOL-TEMP-SCH,     -1, STD, 170, 120, 200, 155, 19, 3, "Cooling T-Stat Sch:",         LEFT, -125, 5, 0, LEFT, 4, 5, "A schedule that specifies the setpoint of the zone cooling thermostat"
    
; SAC 11/30/10 - added for DOE-2.3
      EDIT,  19250, 19250, 0, 1, ZONE, 0, STARTUP-COOL-DT,   -1, STD, 570,  45,  23,  60,  2, 3, "Cooling Design Startup dT:", LEFT, -165, 5, 1, LEFT, 4, 5, "The rate at which the zone temperature can be pulled down during the startup hour"
      EDIT,  19251, 19251, 0, 1, ZONE, 0, RATED-EDB,         -1, STD, 570,  70,  23,  60,  1, 3,    "Rated Entering Drybulb:", LEFT, -165, 5, 1, LEFT, 4, 5, "The indoor entering drybulb corresponding to the cooling capacity"
      EDIT,  19252, 19252, 0, 1, ZONE, 0, RATED-EWB,         -1, STD, 570,  95,  23,  60,  1, 3,    "Rated Entering Wetbulb:", LEFT, -165, 5, 1, LEFT, 4, 5, "The indoor entering wetbulb corresponding to the cooling capacity"
      EDIT,  19253, 19253, 0, 1, ZONE, 0, RATED-ECT,         -1, STD, 570, 120,  23,  60,  1, 3,  "Rated Entering Condenser:", LEFT, -165, 5, 1, LEFT, 4, 5, "The entering condenser temperature corresponding to the cooling capacity"

      LABEL, "Loop Connections",      STD, LEFT,  30, 206, 1, 0, 0, 665, 0, 3

      LABEL, "Chilled Water",         STD, LEFT, 135, 224, 1, 0, 0,   0, 14690, 3
      LABEL, "Condenser Water",       STD, LEFT, 320, 224, 1, 0, 0,   0, 14694, 3
      LABEL, "Water-Side Economizer", STD, LEFT, 505, 224, 1, 0, 0,   0, 14698, 3

      LABEL, "Loop:",                 STD, LEFT,  45, 246, 1, 0, 0,   0,     0, 3
      LABEL, "Valve Type:",           STD, LEFT,  45, 271, 1, 0, 0,   0,     0, 3
      LABEL, "Coil Head:",            STD, LEFT,  45, 296, 1, 0, 0,   0,     0, 3
      LABEL, "Coil Delta T:",         STD, LEFT,  45, 321, 1, 0, 0,   0,     0, 3

      COMBO, 14690, 19077, 0, 1, ZONE, 0, CHW-LOOP,          -1, STD, 130, 243, 200, 165, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "The loop that serves the zonal cooling coil (Loop Type must be Chilled Water or Two Pipe)"
      COMBO, 14691, 13038, 0, 1, ZONE, 0, CHW-VALVE-TYPE,    -1, STD, 130, 268, 100, 110, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
      EDIT,  14692, 13039, 0, 1, ZONE, 0, CHW-COIL-HEAD,     -1, STD, 130, 293,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the coil at the design flowrate"
      EDIT,  14693, 13040, 0, 1, ZONE, 0, CHW-COIL-DT,       -1, STD, 130, 318,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flow rate)"

      COMBO, 14694, 60009, 0, 1, ZONE, 0, CW-LOOP,           -1, STD, 315, 243, 200, 165, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "If Condenser Type=Water Cooled, CW Loop is required & must be attached to a Heat Rejection device"
      COMBO, 14695, 60007, 0, 1, ZONE, 0, CW-VALVE,          -1, STD, 315, 268, 100, 110, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
      EDIT,  14696, 60006, 0, 1, ZONE, 0, CW-COIL-HEAD,      -1, STD, 315, 293,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the condenser at the design flowrate"
      EDIT,  14697, 60008, 0, 1, ZONE, 0, CW-COIL-DT,        -1, STD, 315, 318,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flow rate)"

      COMBO, 14698, 19078, 0, 1, ZONE, 0, WSE-LOOP,          -1, STD, 500, 243, 200, 165, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Name of loop that serves the water-side economizer (Loop Type = Chilled Water or 2 Pipe)"
      COMBO, 14699, 13058, 0, 1, ZONE, 0, WSE-VALVE-TYPE,    -1, STD, 500, 268, 100, 110, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
      EDIT,  14700, 13059, 0, 1, ZONE, 0, WSE-COIL-HEAD,     -1, STD, 500, 293,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the coil at the design flowrate"
      EDIT,  14701, 13060, 0, 1, ZONE, 0, WSE-COIL-DT,       -1, STD, 500, 318,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flow rate)"

; SAC 11/30/10 - added for DOE-2.3
      COMBO, 19254, 19254, 0, 1, ZONE, 0, CONDENSING-UNIT,   -1, STD, 315, 350, 200, 165, 19, 3,    "Condensing Unit:", RIGHT, -5, 5, 0, LEFT, 4, 5, "For a zone served by a CONDENSING-UNIT, the name of the condensing unit"
      EDIT,  19255, 19255, 0, 1, ZONE, 0, TERMINALS/ZONE,    -1, STD, 315, 375,  23,  50,  0, 3, "Num Terminals/Zone:", RIGHT, -5, 5, 1, LEFT, 4, 5, "For a zone served by a CONDENSING-UNIT, specifies the number of indoor-units that are in the zone"


    ;*****************************************
    ; Heating Mode
    ;*****************************************
    TABPAGE, 3047, 29035, 1, 3, NOTIMP, " Heating "
;      LINE,  10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;      COMBO, 19186, 19182, 0, 1, ZONE, 0, NAME,       -1, STD, 260,  10, 200, 200, 19, 3, "Currently Active Zone:", RIGHT, 250, 5, 0, LEFT, 4, 5, "List of all zones defined in project; also allows library retrieval and creation"

      LABEL, "Heating Design Parameters", STD, LEFT,  30,  13, 1, 0, 0, 680, 0, 3
      EDIT,  14702, 12252, 0, 1, ZONE, 0, DESIGN-HEAT-T,     -1, STD, 255,  35,  23,  60,  1, 3, "Heating Design Temperature:", LEFT, -210, 5, 1, LEFT, 4, 5, "Desired space T, used to calculate supply airflow rate required for peak zonal heating loads"
      EDIT,  14703, 13051, 0, 1, ZONE, 0, HEATING-CAPACITY,  -1, STD, 225,  60,  23,  90,  0, 3, "Heating Capacity:",           LEFT, -180, 5, 1, LEFT, 4, 5, "Heating capacity (at ARI conditions) of the zonal heating HVAC system"
      EDIT,  14704, 13026, 0, 1, ZONE, 0, REHEAT-DELTA-T,    -1, STD, 225,  85,  23,  90,  1, 3, "Reheat Delta T:",             LEFT, -180, 5, 1, LEFT, 4, 5, "Maximum increase in supply air temperature due to zonal reheat coils"
      EDIT,  14705, 13030, 0, 1, ZONE, 0, MAX-HEAT-RATE,     -1, STD, 225, 110,  23,  90,  0, 3, "Maximum Heating Rate:",       LEFT, -180, 5, 1, LEFT, 4, 5, "Maximum zonal heating rate, not including baseboards (limits DOE-2's sizing calculation)"
      COMBO, 14706, 12181, 0, 1, ZONE, 0, HEAT-TEMP-SCH,     -1, STD, 165, 135, 300, 165, 19, 3, "Heating T-Stat Sch:",         LEFT, -120, 5, 0, LEFT, 4, 5, "A schedule that specifies the setpoint of the zone heating thermostat"

; SAC 11/30/10 - added for DOE-2.3
      EDIT,  19257, 19257, 0, 1, ZONE, 0, STARTUP-HEAT-DT,   -1, STD, 570,  35,  23,  60,  2, 3,  "Heating Design Startup dT:", LEFT, -165, 5, 1, LEFT, 4, 5, "The rate at which the zone temperature can be raised during the startup hour"
      EDIT,  19258, 19258, 0, 1, ZONE, 0, HT-RATED-EDB,      -1, STD, 570,  60,  23,  60,  1, 3,     "Rated Entering Drybulb:", LEFT, -165, 5, 1, LEFT, 4, 5, "The indoor entering drybulb corresponding to the heating capacity"
      EDIT,  19259, 19259, 0, 1, ZONE, 0, HT-RATED-ECT,      -1, STD, 570,  85,  23,  60,  1, 3, "Rated Entering 'Condenser':", LEFT, -165, 5, 1, LEFT, 4, 5, "The entering 'condenser' temperature corresponding to the heating capacity"

; SAC 10/23/00 - Compliance keyword
; SAC 1/6/10 - removed keywords no longer referenced by T24-08 ruleset (C-REHEAT-CAP)
;       EDIT, 15486,     0, 0, 1, ZONE, 0, C-REHEAT-CAP,      -1, STD, 225, 160,  23,  90,  0, 7, "Reheat Capacity (compliance):", LEFT, -180, 5, 1, LEFT, 4, 5, "The heating capacity of reheating coils for the zone"

;; SAC 10/23/00 - Compliance keyword
;      LABEL, "Exhaust Fan (compliance)", STD, LEFT, 30, 319, 1, 0, 0, 675, 15482, 1
;       EDIT, 15482,     0, 0, 1, ZONE, 0,  C-EXH-FAN-BHP,   -1, STD, 160, 340,  23,  70,  2, 1, "Brake Horsepower:", RIGHT, -5, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15483,     0, 0, 1, ZONE, 0,  C-EF-DRIVE-EFF,  -1, STD, 360, 340,  23,  70,  2, 1, "Drive Efficiency:", RIGHT, -5, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15484,     0, 0, 1, ZONE, 0,  C-EF-MOTOR-EFF,  -1, STD, 580, 340,  23,  70,  2, 1, "Motor Efficiency:", RIGHT, -5, 5, 1, LEFT, 4, 5, ""

      LABEL, "Baseboards",       STD, LEFT,  30, 196, 1, 0, 0, 280, 14707, 3
      EDIT,  14707, 13061, 0, 1, ZONE, 0, BASEBOARD-RATING,  -1, STD, 135, 215,  23, 100,  0, 3, "Capacity:",                   LEFT,  -90, 5, 1, LEFT, 4, 5, "Rated baseboard heating capacity for the zone (required for baseboard simulation)"
; SAC 11/30/10 - added for DOE-2.3
      EDIT,  19256, 19256, 0, 1, ZONE, 0, AUX-HEAT-RATIO,    -1, STD, 135, 240,  23, 100,  2, 3, "Capacity Ratio:",             LEFT,  -90, 5, 1, LEFT, 4, 5, "The fraction of the design zonal heating load that will be picked up by the baseboard"
      COMBO, 14708, 13063, 0, 1, ZONE, 0, BASEBOARD-CTRL,    -1, STD, 135, 265, 200, 145, 19, 3, "Control:",                    LEFT,  -90, 5, 0, LEFT, 4, 5, "Thermostatic=based on zone air T; Outdoor Reset=based on outdoor air T, via reset schedule"
    
      LABEL, "Floor Panel Heat", STD, LEFT, 395, 196, 1, 0, 0, 670, 14709, 3
      EDIT,  14709, 60013, 0, 1, ZONE, 0, PANEL-LOSS-RATIO,  -1, STD, 500, 215,  23,  95,  4, 3, "Loss Ratio:",                 LEFT,  -90, 5, 1, LEFT, 4, 5, "Heat loss from the zonal heating panel (as a fraction of the panel's heating capacity)"

; SAC 10/23/00 - Compliance keyword
      LABEL, "DHW Zone Group", STD, LEFT, 395, 251, 1, 0, 0, 670, 15487, 7
      COMBO, 15487,     0, 0, 1, ZONE, 0, C-COMPLIANCE-DHW,  -1, STD, 500, 270, 300, 170, 19, 7, "DHW Group:",                  LEFT,  -90, 5, 0, LEFT, 4, 5, "The name of the residential water heating group to which this residential zone belongs"

      LABEL, "Loop Connections",  STD, LEFT,  30, 326, 1, 0, 0, 665, 0, 3

      LABEL, "Hot Water",          STD, LEFT, 135, 344, 1, 0, 0,   0, 14710, 3
      LABEL, "Baseboard",          STD, LEFT, 320, 344, 1, 0, 0,   0, 14714, 3
      LABEL, "Domestic Hot Water", STD, LEFT, 505, 344, 1, 0, 0,   0, 14718, 3

      LABEL, "Loop:",              STD, LEFT,  45, 367, 1, 0, 0,   0,     0, 3
      LABEL, "Valve Type:",        STD, LEFT,  45, 392, 1, 0, 0,   0,     0, 3
      LABEL, "Coil Head:",         STD, LEFT,  45, 417, 1, 0, 0,   0,     0, 3
      LABEL, "Coil Delta T:",      STD, LEFT,  45, 442, 1, 0, 0,   0,     0, 3

      COMBO, 14710, 19079, 0, 1, ZONE, 0, HW-LOOP,           -1, STD, 130, 363, 300, 165, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Name of loop that serves the zonal hot water coil (Loop Type=Hot Water, Two Pipe or Steam)"
      COMBO, 14711, 13034, 0, 1, ZONE, 0, HW-VALVE-TYPE,     -1, STD, 130, 388, 100, 110, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
      EDIT,  14712, 13035, 0, 1, ZONE, 0, HW-COIL-HEAD,      -1, STD, 130, 413,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the coil at the design flowrate"
      EDIT,  14713, 13036, 0, 1, ZONE, 0, HW-COIL-DT,        -1, STD, 130, 438,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flow rate)"

      COMBO, 14714, 19086, 0, 1, ZONE, 0, BBRD-LOOP,         -1, STD, 315, 363, 300, 165, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Name of loop that serves baseboard coils (Loop Type must be Hot Water, Two Pipe or Steam)"
      COMBO, 14715, 60011, 0, 1, ZONE, 0, BBRD-VALVE-TYPE,   -1, STD, 315, 388, 100, 110, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
      EDIT,  14716, 13710, 0, 1, ZONE, 0, BBRD-COIL-HEAD,    -1, STD, 315, 413,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the baseboards at the design flowrate"
      EDIT,  14717, 60012, 0, 1, ZONE, 0, BBRD-COIL-DT,      -1, STD, 315, 438,  23,  50,  1, 3, "", LEFT,  -2, 5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flow rate)"

      COMBO, 14718,     0, 0, 1, ZONE, 0, DHW-LOOP,          -1, STD, 500, 363, 300, 165, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, ""

    
    ;*****************************************
    ; Meters Mode
    ;*****************************************
    TABPAGE, 3048, 29035, 1, 3, NOTIMP, " Meters "
;      LINE,  10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;      COMBO, 19187, 19182, 0, 1, ZONE, 0, NAME,       -1, STD, 260,  10, 200, 200, 19, 3, "Currently Active Zone:", RIGHT, 250, 5, 0, LEFT, 4, 5, "List of all zones defined in project; also allows library retrieval and creation"

      LABEL, "Zone-Level Meter Assignments by End-Use:", STD, LEFT, 35, 3, 1, 0, 0, 0, 0, 3
      
      LABEL, "Electric", STD, LEFT, 50, 28, 1, 0, 0, 615, 14719, 3
      COMBO, 14719, 13608, 32079, 1, ZONE, 0,  MSTR-ELEC-METER, 0, STD, 195,  50, 250,  95, 19, 3,  "Master Elec Meter:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies all of the unassigned zone electric consumption"
      COMBO, 14720, 13609, 32079, 1, ZONE, 0, LIGHT-ELEC-METER, 0, STD, 195,  75, 250,  95, 19, 3,      "Area Lighting:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the zone's Area Lighting electric consumption"
      COMBO, 14721, 13610, 32079, 1, ZONE, 0,  TASK-ELEC-METER, 0, STD, 195, 100, 250,  95, 19, 3,      "Task Lighting:", LEFT, -130, 5, 0, LEFT, 4, 5, "Electric Meter that tallies the zone's Task Lighting electricity consumption"
      COMBO, 14722, 13611, 32079, 1, ZONE, 0, EQUIP-ELEC-METER, 0, STD, 195, 125, 250,  95, 19, 3,     "Elec Equipment:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's Equipment electricity consumption"
      COMBO, 14723, 60014, 32079, 1, ZONE, 0, SOURCE-ELEC-METE, 0, STD, 195, 150, 250,  95, 19, 3,        "Source Elec:", LEFT, -130, 5, 0, LEFT, 4, 5, ""
      COMBO, 14724, 13612, 32079, 1, ZONE, 0,  HEAT-ELEC-METER, 0, STD, 195, 175, 250,  95, 19, 3,      "Space Heating:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's Space Heating electricity consumption"
      COMBO, 14725, 13613, 32079, 1, ZONE, 0,  COOL-ELEC-METER, 0, STD, 195, 200, 250,  95, 19, 3,      "Space Cooling:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's Space Cooling electric consumption"

      COMBO, 14726, 60015, 32079, 1, ZONE, 0, HTREJ-ELEC-METER, 0, STD, 520,  75, 250,  95, 19, 3,     "Heat Rejection:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the electric energy required for the zone's heat rejection"
      COMBO, 14727, 60016, 32079, 1, ZONE, 0,   AUX-ELEC-METER, 0, STD, 520, 100, 250,  95, 19, 3,     "Pumps and Misc:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's auxiliary electric energy (e.g., pumps)"
      COMBO, 14728, 13614, 32079, 1, ZONE, 0,  VENT-ELEC-METER, 0, STD, 520, 125, 250,  95, 19, 3,   "Ventilation Fans:", LEFT, -130, 5, 0, LEFT, 4, 5, "Electric Meter that tallies the zone Ventilation Fans electricity consumption"
      COMBO, 14729, 60017, 32079, 1, ZONE, 0,  REFG-ELEC-METER, 0, STD, 520, 150, 250,  95, 19, 3,      "Refrigeration:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's refrigeration electric energy consumption"
      COMBO, 14730, 13616, 32079, 1, ZONE, 0,  SUPP-ELEC-METER, 0, STD, 520, 175, 250,  95, 19, 3,  "Supplemental Heat:", LEFT, -130, 5, 0, LEFT, 4, 5, "Electric Meter that tallies the zone's electric consumption for supplemental heating"
      COMBO, 14731, 13615, 32079, 1, ZONE, 0,   DHW-ELEC-METER, 0, STD, 520, 200, 250,  95, 19, 3, "Domestic Hot Water:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's DHW heater electricity consumption"

      LABEL, "Fuel", STD, LEFT, 50, 243, 1, 0, 0, 615, 14732, 3
      COMBO, 14732, 13617, 32079, 1, ZONE, 0,  MSTR-FUEL-METER, 0, STD, 195, 265, 250,  95, 19, 3,  "Master Fuel Meter:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Fuel Meter that tallies all of the unassigned zone fuel consumption"

      COMBO, 14733, 60018, 32079, 1, ZONE, 0, SOURCE-FUEL-METE, 0, STD, 195, 290, 250,  95, 19, 3,        "Source Fuel:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's 'source' fuel consumption"
      COMBO, 14734, 13618, 32079, 1, ZONE, 0,  HEAT-FUEL-METER, 0, STD, 195, 315, 250,  95, 19, 3,      "Space Heating:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Fuel Meter that tallies all of the unassigned zone fuel consumption"
      COMBO, 14735, 13619, 32079, 1, ZONE, 0,  COOL-FUEL-METER, 0, STD, 195, 340, 250,  95, 19, 3,      "Space Cooling:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of the Fuel Meter that tallies the fuel consumption of this zone's cooling system"

      COMBO, 14736, 13620, 32079, 1, ZONE, 0,  SUPP-FUEL-METER, 0, STD, 520, 290, 250,  95, 19, 3,  "Supplemental Heat:", LEFT, -130, 5, 0, LEFT, 4, 5, "Electric Meter that tallies the zone's fuel consumption for supplemental heating"
      COMBO, 14737, 13621, 32079, 1, ZONE, 0,   DHW-FUEL-METER, 0, STD, 520, 315, 250,  95, 19, 3, "Domestic Hot Water:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's DHW heater fuel consumption"


; SAC 11/24/10 - removed entire tab    
;    ;*****************************************
;    ; Refrig Mode
;    ;*****************************************
;    TABPAGE, 3049, 29035, 1, 3, NOTIMP, " Refrigeration "
;;      LINE,  10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;;      COMBO, 19188, 19182, 0, 1, ZONE, 0, NAME,       -1, STD, 260,  10, 200, 200, 19, 3, "Currently Active Zone:", RIGHT, 250, 5, 0, LEFT, 4, 5, "List of all zones defined in project; also allows library retrieval and creation"
;
;      LABEL, "Evaporator",  STD, LEFT,    25,   7, 1, 0, 0, 0,     0, 3
;      LABEL, "Temperature", STD, LEFT,    25,  23, 1, 0, 0, 0,     0, 3
;      LABEL, "Ranges:",     STD, LEFT,    25,  39, 1, 0, 0, 0,     0, 3
;
;      LABEL, "Zone Load",   STD, CENTER, 155,  23, 1, 0, 0, 0, 14738, 3
;      LABEL, "Sensible",    STD, CENTER, 250,   7, 1, 0, 0, 0, 14741, 3
;      LABEL, "Heat",        STD, CENTER, 250,  23, 1, 0, 0, 0, 14741, 3
;      LABEL, "Case",        STD, CENTER, 335,   7, 1, 0, 0, 0, 14744, 3
;      LABEL, "Temperature", STD, CENTER, 335,  23, 1, 0, 0, 0, 14744, 3
;      LABEL, "Evaporator",  STD, CENTER, 420,   7, 1, 0, 0, 0, 14747, 3
;      LABEL, "Temperature", STD, CENTER, 420,  23, 1, 0, 0, 0, 14747, 3
;      LABEL, "Design",      STD, CENTER, 515,   7, 1, 0, 0, 0, 14750, 3
;      LABEL, "Temperature", STD, CENTER, 515,  23, 1, 0, 0, 0, 14750, 3
;      LABEL, "Design",      STD, CENTER, 600,   7, 1, 0, 0, 0, 14753, 3
;      LABEL, "Rel. Hum.",   STD, CENTER, 600,  23, 1, 0, 0, 0, 14753, 3
;
;      LABEL, "coldest:",    STD, LEFT,    40,  60, 1, 0, 0, 0,     0, 3
;      LABEL, "medium:",     STD, LEFT,    40,  85, 1, 0, 0, 0,     0, 3
;      LABEL, "warmest:",    STD, LEFT,    40, 110, 1, 0, 0, 0,     0, 3
;
;      EDIT,  14738, 13623, 751, 1, ZONE, 0, REFG-ZONE-LOAD,   0, STD, 110,  55,  23,  90,  0, 3, "", LEFT,  -2, 5, 1, CENTER, -45, -16, "Total cooling to zone due to air from open refrigeration cases, and heat radiating to the cases"
;      EDIT,  14739, 13623, 751, 1, ZONE, 0, REFG-ZONE-LOAD,   1, STD, 110,  80,  23,  90,  0, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Total cooling to zone due to air from open refrigeration cases, and heat radiating to the cases"
;      EDIT,  14740, 13623, 751, 1, ZONE, 0, REFG-ZONE-LOAD,   2, STD, 110, 105,  23,  90,  0, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Total cooling to zone due to air from open refrigeration cases, and heat radiating to the cases"
;    
;      EDIT,  14741, 13626, 751, 1, ZONE, 0, REFG-ZONE-SHR,    0, STD, 215,  55,  23,  70,  3, 3, "", LEFT,  -2, 5, 1, CENTER, -35, -16, "Ratio of sensible to total heat removed from zone by refrigeration cases"
;      EDIT,  14742, 13626, 751, 1, ZONE, 0, REFG-ZONE-SHR,    1, STD, 215,  80,  23,  70,  3, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Ratio of sensible to total heat removed from zone by refrigeration cases"
;      EDIT,  14743, 13626, 751, 1, ZONE, 0, REFG-ZONE-SHR,    2, STD, 215, 105,  23,  70,  3, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Ratio of sensible to total heat removed from zone by refrigeration cases"
;    
;      EDIT,  14744, 13635, 751, 1, ZONE, 0, REFG-DISCHARGE-T, 0, STD, 300,  55,  23,  70,  1, 3, "", LEFT,  -2, 5, 1, CENTER, -35, -16, "Temperature of air inside the refrigeration casework (at the coldest of the three evaporator Ts)"
;      EDIT,  14745, 13635, 751, 1, ZONE, 0, REFG-DISCHARGE-T, 1, STD, 300,  80,  23,  70,  1, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Temperature of air inside the refrigeration casework (at the middle of the three evaporator Ts)"
;      EDIT,  14746, 13635, 751, 1, ZONE, 0, REFG-DISCHARGE-T, 2, STD, 300, 105,  23,  70,  1, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Temperature of air inside the refrigeration casework (at the warmest of the three evaporator Ts)"
;    
;      EDIT,  14747, 60019, 751, 1, ZONE, 0, REFG-EVAP-T,      0, STD, 385,  55,  23,  70,  1, 3, "", LEFT,  -2, 5, 1, CENTER, -35, -16, "Coldest of the three dewpoint temperatures at which the evaporator operates"
;      EDIT,  14748, 60019, 751, 1, ZONE, 0, REFG-EVAP-T,      1, STD, 385,  80,  23,  70,  1, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Middle of the three dewpoint temperatures at which the evaporator operates"
;      EDIT,  14749, 60019, 751, 1, ZONE, 0, REFG-EVAP-T,      2, STD, 385, 105,  23,  70,  1, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Warmest of the three dewpoint temperatures at which the evaporator operates"
;    
;      EDIT,  14750, 60022, 751, 1, ZONE, 0, REFG-ZONE-DES-T,  0, STD, 480,  55,  23,  70,  1, 3, "", LEFT,  -2, 5, 1, CENTER, -35, -16, "Drybulb temperature of zone air at which the refrigeration casework is rated (typically 75%)"
;      EDIT,  14751, 60022, 751, 1, ZONE, 0, REFG-ZONE-DES-T,  1, STD, 480,  80,  23,  70,  1, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Drybulb temperature of zone air at which the refrigeration casework is rated (typically 75%)"
;      EDIT,  14752, 60022, 751, 1, ZONE, 0, REFG-ZONE-DES-T,  2, STD, 480, 105,  23,  70,  1, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Drybulb temperature of zone air at which the refrigeration casework is rated (typically 75%)"
;    
;      EDIT,  14753, 60023, 751, 1, ZONE, 0, REFG-ZONE-DES-RH, 0, STD, 565,  55,  23,  70,  1, 3, "", LEFT,  -2, 5, 1, CENTER, -35, -16, "Relative Humidity of zone air at which the refrigeration casework is rated (typically 55%)"
;      EDIT,  14754, 60023, 751, 1, ZONE, 0, REFG-ZONE-DES-RH, 1, STD, 565,  80,  23,  70,  1, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Relative Humidity of zone air at which the refrigeration casework is rated (typically 55%)"
;      EDIT,  14755, 60023, 751, 1, ZONE, 0, REFG-ZONE-DES-RH, 2, STD, 565, 105,  23,  70,  1, 3, "", LEFT,  -2, 5, 0, CENTER,   4,   5, "Relative Humidity of zone air at which the refrigeration casework is rated (typically 55%)"
;
;      LABEL, "Covers",          STD, LEFT,   110, 143, 1, 0, 0, 380, 14756, 3
;      LABEL, "Sensible Sched",  STD, CENTER, 170, 159, 1, 0, 0,   0, 14756, 3
;      LABEL, "Latent Sched",    STD, CENTER, 310, 159, 1, 0, 0,   0, 14759, 3
;      LABEL, "Defrost",         STD, LEFT,   400, 143, 1, 0, 0, 670, 14762, 3
;      LABEL, "Type",            STD, CENTER, 445, 159, 1, 0, 0,   0, 14762, 3
;      LABEL, "Control",         STD, CENTER, 550, 159, 1, 0, 0,   0, 14765, 3
;      LABEL, "Efficiency",      STD, CENTER, 640, 159, 1, 0, 0,   0, 14768, 3
;
;      LABEL, "coldest:",   STD,        LEFT,    40, 180, 1, 0, 0, 0,     0, 3
;      LABEL, "medium:",    STD,        LEFT,    40, 205, 1, 0, 0, 0,     0, 3
;      LABEL, "warmest:",   STD,        LEFT,    40, 230, 1, 0, 0, 0,     0, 3
;
;      COMBO, 14756, 60020, 751, 1, ZONE, 0, REFG-SENS-SCH,    0, STD, 110, 175, 200, 130, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Used to simulate covers on refrigeration casework that inhibit sensible cooling effect to zone"
;      COMBO, 14757, 60020, 751, 1, ZONE, 0, REFG-SENS-SCH,    1, STD, 110, 200, 200, 130, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Used to simulate covers on refrigeration casework that inhibit sensible cooling effect to zone"
;      COMBO, 14758, 60020, 751, 1, ZONE, 0, REFG-SENS-SCH,    2, STD, 110, 225, 200, 130, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Used to simulate covers on refrigeration casework that inhibit sensible cooling effect to zone"
;    
;      COMBO, 14759, 60021, 751, 1, ZONE, 0, REFG-LAT-SCH,     0, STD, 250, 175, 200, 130, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Used to simulate covers on refrigeration casework that inhibit latent cooling effect to zone"
;      COMBO, 14760, 60021, 751, 1, ZONE, 0, REFG-LAT-SCH,     1, STD, 250, 200, 200, 130, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Used to simulate covers on refrigeration casework that inhibit latent cooling effect to zone"
;      COMBO, 14761, 60021, 751, 1, ZONE, 0, REFG-LAT-SCH,     2, STD, 250, 225, 200, 130, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Used to simulate covers on refrigeration casework that inhibit latent cooling effect to zone"
;    
;      COMBO, 14762, 13629, 751, 1, ZONE, 0, REFG-DEF-MECH,    0, STD, 400, 175, 140,  95, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Resistance=electric coils; Freon=hot gas defrost; Time-Off=timed off cycle; No Defrost=none"
;      COMBO, 14763, 13629, 751, 1, ZONE, 0, REFG-DEF-MECH,    1, STD, 400, 200, 140,  95, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Resistance=electric coils; Freon=hot gas defrost; Time-Off=timed off cycle; No Defrost=none"
;      COMBO, 14764, 13629, 751, 1, ZONE, 0, REFG-DEF-MECH,    2, STD, 400, 225, 140,  95, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Resistance=electric coils; Freon=hot gas defrost; Time-Off=timed off cycle; No Defrost=none"
;    
;      COMBO, 14765, 13632, 751, 1, ZONE, 0, REFG-DEF-CTRL,    0, STD, 505, 175, 140,  95, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, ""
;      COMBO, 14766, 13632, 751, 1, ZONE, 0, REFG-DEF-CTRL,    1, STD, 505, 200, 140,  95, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, ""
;      COMBO, 14767, 13632, 751, 1, ZONE, 0, REFG-DEF-CTRL,    2, STD, 505, 225, 140,  95, 19, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, ""
;    
;      EDIT,  14768, 60027, 751, 1, ZONE, 0, REFG-DEF-EFF,     0, STD, 610, 175,  23,  60,  2, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Efficiency of the fefroster (if one exists, see Refrigeration Defrost Type)"
;      EDIT,  14769, 60027, 751, 1, ZONE, 0, REFG-DEF-EFF,     1, STD, 610, 200,  23,  60,  2, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Efficiency of the fefroster (if one exists, see Refrigeration Defrost Type)"
;      EDIT,  14770, 60027, 751, 1, ZONE, 0, REFG-DEF-EFF,     2, STD, 610, 225,  23,  60,  2, 3, "", LEFT,  -2, 5, 0, LEFT, 4, 5, "Efficiency of the fefroster (if one exists, see Refrigeration Defrost Type)"
;
;      LABEL, "Auxiliaries",  STD, LEFT,   110, 263, 1, 0, 0, 450, 14771, 3
;      LABEL, "kW",           STD, CENTER, 140, 279, 1, 0, 0,   0, 14771, 3
;      LABEL, "Btu/hr",       STD, CENTER, 220, 279, 1, 0, 0,   0, 14774, 3
;      LABEL, "Schedule",     STD, CENTER, 355, 279, 1, 0, 0,   0, 14777, 3
;
;      LABEL, "coldest:",     STD, LEFT,    40, 300, 1, 0, 0,   0,     0, 3
;      LABEL, "medium:",      STD, LEFT,    40, 325, 1, 0, 0,   0,     0, 3
;      LABEL, "warmest:",     STD, LEFT,    40, 350, 1, 0, 0,   0,     0, 3
;
;      EDIT,  14771, 60024, 751, 1, ZONE, 0, REFG-AUX-KW,      0, STD, 110, 295,  23,  60,  2, 3, "", LEFT,  -2, 5, 0, CENTER, 4, 5, "Rated electric consumption of equipment within the refrigeration casework (lights, fans, etc.)"
;      EDIT,  14772, 60024, 751, 1, ZONE, 0, REFG-AUX-KW,      1, STD, 110, 320,  23,  60,  2, 3, "", LEFT,  -2, 5, 0, CENTER, 4, 5, "Rated electric consumption of equipment within the refrigeration casework (lights, fans, etc.)"
;      EDIT,  14773, 60024, 751, 1, ZONE, 0, REFG-AUX-KW,      2, STD, 110, 345,  23,  60,  2, 3, "", LEFT,  -2, 5, 0, CENTER, 4, 5, "Rated electric consumption of equipment within the refrigeration casework (lights, fans, etc.)"
;
;      EDIT,  14774, 60025, 751, 1, ZONE, 0, REFG-AUX-HEAT,    0, STD, 180, 295,  23,  80,  0, 3, "", LEFT,  -2, 5, 0, CENTER, 4, 5, "Rated fuel consumption associated with refrigeration (e.g., resurfacing ice rinks with hot water)"
;      EDIT,  14775, 60025, 751, 1, ZONE, 0, REFG-AUX-HEAT,    1, STD, 180, 320,  23,  80,  0, 3, "", LEFT,  -2, 5, 0, CENTER, 4, 5, "Rated fuel consumption associated with refrigeration (e.g., resurfacing ice rinks with hot water)"
;      EDIT,  14776, 60025, 751, 1, ZONE, 0, REFG-AUX-HEAT,    2, STD, 180, 345,  23,  80,  0, 3, "", LEFT,  -2, 5, 0, CENTER, 4, 5, "Rated fuel consumption associated with refrigeration (e.g., resurfacing ice rinks with hot water)"
;
;      COMBO, 14777, 60026, 751, 1, ZONE, 0, REFG-AUX-SCH,     0, STD, 270, 295, 200, 180, 19, 3, "", LEFT,  -2, 5, 0, LEFT,   4, 5, "On-off schedule, applies to both auxiliary electrical and auxiliary heat loads"
;      COMBO, 14778, 60026, 751, 1, ZONE, 0, REFG-AUX-SCH,     1, STD, 270, 320, 200, 180, 19, 3, "", LEFT,  -2, 5, 0, LEFT,   4, 5, "On-off schedule, applies to both auxiliary electrical and auxiliary heat loads"
;      COMBO, 14779, 60026, 751, 1, ZONE, 0, REFG-AUX-SCH,     2, STD, 270, 345, 200, 180, 19, 3, "", LEFT,  -2, 5, 0, LEFT,   4, 5, "On-off schedule, applies to both auxiliary electrical and auxiliary heat loads"


    ;*****************************************
    ; Sun Space Mode
    ;*****************************************
    TABPAGE, 3050, 29035, 1, 3, NOTIMP, " Sun Space "
;      LINE,  10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;      COMBO, 19189, 19182, 0, 1, ZONE, 0, NAME,       -1, STD, 260,  10, 200, 200, 19, 3, "Currently Active Zone:", RIGHT, 250, 5, 0, LEFT, 4, 5, "List of all zones defined in project; also allows library retrieval and creation"

      LABEL, "Sunspace Heat to Adjacent Zones", STD, LEFT,  30,  52, 1, 0, 0, 350, 14780, 3
      COMBO, 14780, 60029, 753, 1, ZONE, 0, SS-FLOW-SCH,      -1, STD, 215,  75, 200, 135, 19, 3, "Air Flow Modifier Sched:",    LEFT, -170, 5, 0, LEFT, 4, 5, "A scheduled multiplier on the air flow across an Interior Wall in a Sunspace"
      COMBO, 14781, 60028, 753, 1, ZONE, 0, SS-FLOW-T-SCH,    -1, STD, 215, 100, 200, 135, 19, 3, "Air Flow T Threshold Sched:", LEFT, -170, 5, 0, LEFT, 4, 5, "If the temp of Next To space is above this, air doesn't flow into that space from the Sunspace"

      LABEL, "Sunspace Venting (overheating)", STD, LEFT,  30, 167, 1, 0, 0, 350, 14782, 3
      COMBO, 14782, 60034, 753, 1, ZONE, 0, SS-VENT-SCH,      -1, STD, 215, 190, 200, 135, 19, 3, "Venting Schedule:",           LEFT, -170, 5, 0, LEFT, 4, 5, "On-off schedule that specifies when a Sunspace can be ventilated"
      COMBO, 14783, 60033, 753, 1, ZONE, 0, SS-VENT-T-SCH,    -1, STD, 215, 215, 200, 135, 19, 3, "Venting T Threshold Sched:",  LEFT, -170, 5, 0, LEFT, 4, 5, "If the Sunspace air is above this temperature, ventilation is allowed"
      EDIT,  14784, 60035, 753, 1, ZONE, 0, SS-VENT-LIMIT-T,  -1, STD, 215, 240,  23,  60,  1, 3, "Venting Limit Temperature:",  LEFT, -170, 5, 1, LEFT, 4, 5, "If outside air drybulb is below this scheduled temperature, ventilation is allowed"
      EDIT,  14785, 60036, 753, 1, ZONE, 0, SS-VENT-KW/FLOW,  -1, STD, 215, 265,  23,  60,  2, 3, "Venting kW:",                 LEFT, -170, 5, 1, LEFT, 4, 5, "Electric consumption of the Sunspace vent fan, per unit air flow (i.e., in units of kW/cfm)"

      LABEL, "Natural Convection Venting (coeffs)", STD, LEFT, 430, 167, 1, 0, 0, 660, 14786, 3
      EDIT,  14786, 60030, 753, 1, ZONE, 0, SS-VENT-CST,      -1, STD, 535, 190,  23,  80,  4, 3, "Constant:",                   LEFT,  -90, 5, 1, LEFT, 4, 5, "Used to calculate the # of outside air changes per hour in Sunspace due to natural convection"
      EDIT,  14787, 60031, 753, 1, ZONE, 0, SS-VENT-WND,      -1, STD, 535, 215,  23,  80,  4, 3, "Wind:",                       LEFT,  -90, 5, 1, LEFT, 4, 5, "Used to calculate the # of outside air changes per hour in Sunspace due to natural convection"
      EDIT,  14788, 60032, 753, 1, ZONE, 0, SS-VENT-TEMP,     -1, STD, 535, 240,  23,  80,  4, 3, "Temperature:",                LEFT,  -90, 5, 1, LEFT, 4, 5, "Used to calculate the # of outside air changes per hour in Sunspace due to natural convection"


 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     HVAC System - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
;PV - addition to SYSTEM command
; 146> ZONE-CHW-LOOP                       Symbolic Defined    1   62 (CIRCULATION-LOOP)  TABLE =4  145         -8 (*  Unused  *    )
;            NOTE: input to ZONE-CHW-LOOP    MUST be a CIRCULATION-LOOP of TYPE =CHW                             [ISYMTB(n, 482)]
;                                                                       or TYPE =PIPE2                           [ISYMTB(n, 483)]

; MODTABDLG, 3051, 2013, 1,  50, 100, 350, 600, 0, "System Type:  ", SYSTEM, 0, TYPE, 0, 0, 0, "     System Name:  ", SYSTEM, 0, NAME, 0, 0, 0, ""
; MODTABDLG, 3051, 2013, 1, 30, 30, 470, 710, 0, SYSTEM, "Air-Side HVAC System Parameters", NOTIMP, 0, NOTIMP, 0
; SAC 4/23/09 - increased dialog size from "470, 710" to "570, 1030"
; AFR 7/22/09 - increased dialog height from 570 ro 580
MODTABDLG, 3051, 2013, 1, 30, 30, 580, 1030, 0, SYSTEM, "Air-Side HVAC System Parameters", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 19196, 19196, 0, 1, SYSTEM, 0, NAME, 0, STD, 210,  15, 400, 250, 19, 3, "Currently Active System:", LEFT, -150, 5, 0, LEFT, 4, 5, "List of all HVAC systems defined in project; also allows library retrieval and creation"
   STATIC, 1, SYSTEM, 0, TYPE, 0, 0, 0, 485, 20, 250, STD, LEFT, "System Type:  ",   "", 0, 3

    ;*****************************************
    ; Basic Specifications
    ;*****************************************
    TABPAGE, 3052, 2013, 1, 3, NOTIMP, "  Basics  "
    
       EDIT, 13076, 13076, 0, 1, SYSTEM, 0,             NAME, 0, STD, 120,   7,  23, 190, 32, 3,      "System Name:", LEFT,  -90, 5, 0, LEFT, 4, 5, "Name of zone; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 19021, 19064, 0, 1, SYSTEM, 0,             TYPE, 0, STD, 120,  32, 390, 190, 19, 3,      "System Type:", LEFT,  -90, 5, 0, LEFT, 4, 5, ""

; SAC 11/24/10 - shifted entire left column up 1 row to accommodate design sizing keywords
      LABEL, "General Parameters", STD, LEFT, 30, 63, 1, 0, 0, 310, 0, 3
      COMBO, 13106, 13084, 0, 1, SYSTEM, 0,  RETURN-AIR-PATH, 0, STD, 150,  80, 100, 160, 19, 3,  "Return Air Path:", LEFT, -105, 5, 0, LEFT, 4, 5, ""
      COMBO, 14250, 14249, 0, 1, SYSTEM, 0,     CONTROL-ZONE, 0, STD, 150, 105, 300, 160, 19, 3,     "Control Zone:", LEFT, -105, 5, 0, LEFT, 4, 5, "The zone that is the easiest to heat in the winter and the hardest to cool in the summer"
      COMBO, 13107, 13107, 0, 1, SYSTEM, 0,   SYSTEM-REPORTS, 0, STD, 150, 130,  85, 160, 19, 3,   "System Reports:", LEFT, -105, 5, 0, LEFT, 4, 5, ""
      COMBO, 13097, 13097, 0, 1, SYSTEM, 0,         DDS-TYPE, 0, STD, 150, 155, 100, 160, 19, 3,   "Dual Duct Type:", LEFT, -105, 5, 0, LEFT, 4, 5, ""
;     COMBO, 13156, 13156, 0, 1, SYSTEM, 0,            *COST, 0, STD, 150, 180, 120, 160, 19, 3,             "Cost:", LEFT, -105, 5, 0, LEFT, 4, 5, ""
; JJH 1/17/06 - GSHP mods
; SDG 3/22/13 – Hybrid mods
      COMBO, 17957,     0, 0, 1, SYSTEM, 0,    WLHP-CATEGORY, 0, STD, 150, 180, 120, 160, 19, 3,    "WL/GS Ht Pump:", LEFT, -105, 5, 0, LEFT, 4, 5, "Rating category of a water-cooled DX system, such as a water loop/ground source heat pump"

; SAC 8/25/09 - minor re-positioning
      LABEL,    "System Sizing", STD, LEFT, 30, 210, 1, 0, 0, 310, 0, 3
       EDIT, 13109, 13087, 0, 1, SYSTEM, 0,     SIZING-RATIO, 0, STD, 150, 230,  23,  50,  2, 3,     "Sizing Ratio:", LEFT, -105, 5, 1, LEFT, 4, 5, ""
      COMBO, 13108, 13108, 0, 1, SYSTEM, 0,    SIZING-OPTION, 0, STD, 150, 255,  80, 160, 19, 3,    "Sizing Option:", LEFT, -105, 5, 0, LEFT, 4, 5, ""
; SAC 3/2/11 - added SIZING-METHOD & FLOW/CAPACITY
      COMBO, 19323, 19323, 0, 1, SYSTEM, 0,    SIZING-METHOD, 0, STD, 150, 280,  80, 160, 19, 3,    "Sizing Method:", LEFT, -105, 5, 0, LEFT, 4, 5, "Specifies whether airflow and cooling capacity are related, and which takes precedence"
       EDIT, 19324, 19324, 0, 1, SYSTEM, 0,    FLOW/CAPACITY, 0, STD, 160, 305,  23,  50,  0, 3,    "Flow/Capacity:", LEFT, -115, 5, 1, LEFT, 4, 5, "The nominal ratio of airflow to cooling capacity"
; DEM 11/28/16 - new keywords
       EDIT, 19481, 19481, 0, 1, SYSTEM, 0, MAX-FLOW/CAPACIT, 0, STD, 160, 330,  23,  50,  0, 3, "Max Flow/Capacity:", LEFT, -115, 5, 1, LEFT, 4, 5, "The maxumum ratio of airflow to cooling capacity"
       EDIT, 19482, 19482, 0, 1, SYSTEM, 0, MIN-FLOW/CAPACIT, 0, STD, 160, 355,  23,  50,  0, 3, "Min Flow/Capacity:", LEFT, -115, 5, 1, LEFT, 4, 5, "The minimum ratio of airflow to cooling capacity"
       EDIT, 19231, 19231, 0, 1, SYSTEM, 0,  HEAT-SUP/RET-DT, 0, STD, 160, 380,  23,  50,  2, 3,  "Heat Sup/Ret dT:", LEFT, -115, 5, 1, LEFT, 4, 5, "The design heating differential between the zonal supply and return temperatures for airflow sizing"
       EDIT, 19232, 19232, 0, 1, SYSTEM, 0,  COOL-SUP/RET-DT, 0, STD, 160, 405,  23,  50,  2, 3,  "Cool Sup/Ret dT:", LEFT, -115, 5, 1, LEFT, 4, 5, "The design cooling differential between the zonal supply and return temperatures for airflow sizing"

; SAC 3/2/11 - added new Unit Staging group w/ NUMBER-OF-UNITS & UNIT-STAGING
      LABEL,    "Unit Staging", STD, LEFT, 30, 435, 1, 0, 0, 310, 0, 3
       EDIT, 19325, 19325, 0, 1, SYSTEM, 0,  NUMBER-OF-UNITS, 0, STD, 150, 454,  23,  50,  0, 3,  "Number of Units:", LEFT, -105, 5, 1, LEFT, 4, 5, "The number of identical units serving the zone(s)"
      COMBO, 19326, 19326, 0, 1, SYSTEM, 0,     UNIT-STAGING, 0, STD, 150, 479,  80, 160, 19, 3,  "Staging Control:", LEFT, -105, 5, 0, LEFT, 4, 5, "For single-zone systems, whether all units run in parallel or stage sequentially with load"

; SAC 5/13/10 - comment out access to PERFORMANCE-DATA components until implementation completed
;; JJH added performance data reference
;      LABEL,    "DX Performance Data", STD, LEFT, 30, 315, 1, 0, 0, 310, 0, 3
;      COMBO, 18969, 13108, 0, 1, SYSTEM, 0, PERFORM-DATA-AC , 0, STD, 150, 335,  80, 160, 19, 3,       "DX Cooling:", LEFT, -105, 5, 0, LEFT, 4, 5, ""
;      COMBO, 18970, 13108, 0, 1, SYSTEM, 0, PERFORM-DATA-HP , 0, STD, 150, 360,  80, 160, 19, 3,     "DX Heat/Cool:", LEFT, -105, 5, 0, LEFT, 4, 5, ""

;     LABEL,    "Gas Pump Auxiliary Electric", STD, LEFT, 18, 228, 1, 0, 0, 0, 0, 3
;      EDIT, 14513, 14513, 0, 1, SYSTEM, 0,   UNIT-PUMP-ELEC, 0, STD, 120, 250,  23,  50,  3, 3,      "GHP Pump kW:", LEFT, -100, 5, 1, LEFT, 4, 5, "Pump power for the Gas Heat Pump, or supplemental boiler (per Btu Cooling Capacity)"
;      EDIT, 14514, 14514, 0, 1, SYSTEM, 0,      UNIT-AUX-KW, 0, STD, 120, 275,  23,  50,  3, 3,       "GHP Aux kW:", LEFT, -100, 5, 1, LEFT, 4, 5, ""

; SAC 3/2/11 - shifted this group of controls down to make room for 
; SAC 3/2/11 - compressed controls over to right to allow for several new controls in the first column of dialog box
      LABEL,    "Cooling", STD, LEFT, 518, 423, 1, 0, 0, 0, 0, 7
      LABEL,    "Heating", STD, LEFT, 767, 423, 1, 0, 0, 0, 0, 7
; AFR 4/29/09 - equip data here from Compliance/Cooling
          EDIT, 15573, 15573, 0, 1, SYSTEM, 0, C-CLG-EQUIP-MFRG, -1, STD, 513, 440,  23, 244, 76, 7,       "Equip Manufacturer(s):", LEFT, -150, 5, 1, LEFT, 4, 5, "The manufacturer of the primary cooling equipment of the system"
          EDIT, 15574, 15574, 0, 1, SYSTEM, 0, C-CLG-EQUIP-MNUM, -1, STD, 513, 465,  23, 244, 76, 7,       "Equip Model Number(s):", LEFT, -150, 5, 1, LEFT, 4, 5, "The model number of the primary cooling equipment of the system"
; AFR 7/15/09 - equip data here from Compliance/Heating
          EDIT, 15582, 15582, 0, 1, SYSTEM, 0, C-HTG-EQUIP-MFRG, -1, STD, 762, 440,  23, 243, 76, 7,   "",                           LEFT, -150, 5, 1, LEFT, 4, 5, "The manufacturer of the primary heating equipment of the system"
          EDIT, 15583, 15583, 0, 1, SYSTEM, 0, C-HTG-EQUIP-MNUM, -1, STD, 762, 465,  23, 243, 76, 7,   "",                           LEFT, -150, 5, 1, LEFT, 4, 5, "The model number of the primary heating equipment of the system"

; AFR 7/15/09 - moved here from Compliance Reporting tab per KJM    - SAC 8/25/09 - minor re-positioning    - SAC 3/9/10 - switched flag value from 7 -> 8 to enable access when jurisdictional QC reporting selected
          EDIT, 15543, 15543, 0, 1, SYSTEM, 0,   C-NUM-OF-UNITS, 0, STD, 513, 260,  23,  80,  0, 8,           "Number of Units:", LEFT, -150, 5, 1, LEFT, 4, 5, "The number of identical units"
         COMBO, 15557, 15557, 0, 1, SYSTEM, 0,    C-HAS-HTG-CLG, 0, STD, 513, 285, 300, 145, 19, 7,           "System Used For:", LEFT, -150, 5, 0, LEFT, 4, 5, "The type of system (heating/cooling/both)"
         COMBO, 15549, 15549, 0, 1, SYSTEM, 0,    C-FURN-CONFIG, 0, STD, 513, 310, 300, 145, 19, 7,     "Furnace Configuration:", LEFT, -150, 5, 0, LEFT, 4, 5, "The configuration of the furnace"
         COMBO, 15546, 15546, 0, 1, SYSTEM, 0,      C-HP-CONFIG, 0, STD, 513, 335, 300, 145, 19, 7,   "Heat Pump Configuration:", LEFT, -150, 5, 0, LEFT, 4, 5, "The configuration of the heat pump"
         COMBO, 15545, 15545, 0, 1, SYSTEM, 0,      C-AC-CONFIG, 0, STD, 513, 360, 300, 145, 19, 7,   "Air Cond. Configuration:", LEFT, -150, 5, 0, LEFT, 4, 5, "The configuration of the air conditioner"

; AFR 4/29/09 - moved all right side controls right
; SAC 11/24/10 - moved into center section and split into multiple columns to allow room for new design sizing keywords
      LABEL,    "Duct Losses", STD, LEFT, 385, 10, 1, 0, 0, 1005, 13099, 3
       EDIT, 13099, 13099, 0, 1, SYSTEM, 0,    DUCT-AIR-LOSS, 0, STD, 505,  30,  23,  50,  2, 3,    "Duct Air Loss:", LEFT, -105, 5, 1, LEFT, 4, 5, "Fraction of the supply air that is lost from the ductwork (to the Duct Zone)"
   ; SAC 5/14/08 - added AIR-LOSS-TYPE combobox
      COMBO, 18973, 13099, 0, 1, SYSTEM, 0,    AIR-LOSS-TYPE, 0, STD, 505,  55, 300, 150, 19, 3,    "Air Loss Type:", LEFT, -105, 5, 0, LEFT, 4, 5, "Duct air loss is Constant (independent of airflow, except if the fan is cycling), or Proportional (varies in proportion to airflow)"
       EDIT, 17914, 17914, 0, 1, SYSTEM, 0, DUCT-AIR-LOSS-OA, 0, STD, 505,  80,  23,  50,  2, 3, "Duct Air Loss OA:", LEFT, -105, 5, 1, LEFT, 4, 5, "Fraction of the supply duct air loss that is made up by outside air"
      COMBO, 13104, 13104, 0, 1, SYSTEM, 0,        DUCT-ZONE, 0, STD, 505, 105, 300, 150, 19, 3,        "Duct Zone:", LEFT, -105, 5, 0, LEFT, 4, 5, "Name of the zone that contains the supply and return ducts (and receives duct thermal losses and air leakage)"
; SAC 11/24/10 - added several design sizing keywords
      LABEL,    "Supply", STD, CENTER, 805, 38, 1, 0, 0, 0, 13100, 3
       EDIT, 13100, 13100, 0, 1, SYSTEM, 0,          DUCT-UA, 0, STD, 780,  55,  23,  50,  2, 3,          "Duct UA:", LEFT,  -90, 5, 0, LEFT, 4, 5, "Overall thermal conductivity of the supply ductwork (this is an alternative to Duct Delta T)"
       EDIT, 13101, 13101, 0, 1, SYSTEM, 0,          DUCT-DT, 0, STD, 780,  80,  23,  50,  2, 3,     "Duct Delta T:", LEFT,  -90, 5, 0, LEFT, 4, 5, "Temp decrease in the hot ducts (and increase in cold ducts) due to heat loss through ducts"
       EDIT, 19226, 19226, 0, 1, SYSTEM, 0,    DUCT-ENVIR-DT, 0, STD, 780, 105,  23,  50,  2, 3,    "Duct-Envir dT:", LEFT,  -90, 5, 0, LEFT, 4, 5, "The design differential between the air temperature entering the duct, and the duct's environment"
      LABEL,    "Return", STD, CENTER, 865, 38, 1, 0, 0, 0, 17887, 3
       EDIT, 17887, 13100, 0, 1, SYSTEM, 0,        RETURN-UA, 0, STD, 840,  55,  23,  50,  2, 3,                  "", LEFT,   -1, 5, 0, LEFT, 4, 5, "Overall thermal conductivity of the return ductwork"
       EDIT, 19227, 19227, 0, 1, SYSTEM, 0,        RETURN-DT, 0, STD, 840,  80,  23,  50,  2, 3,                  "", LEFT,   -1, 5, 0, LEFT, 4, 5, "Return duct temperature change at design conditions"
       EDIT, 19228, 19228, 0, 1, SYSTEM, 0,  RETURN-ENVIR-DT, 0, STD, 840, 105,  23,  50,  2, 3,                  "", LEFT,   -1, 5, 0, LEFT, 4, 5, "The design differential between the air temperature entering the return duct, and the duct's environment"
      LABEL,    "Hot", STD, CENTER, 925, 38, 1, 0, 0, 0, 13102, 3
       EDIT, 13102, 13102, 0, 1, SYSTEM, 0,      HOT-DUCT-UA, 0, STD, 900,  55,  23,  50,  2, 3,                  "", LEFT,   -1, 5, 1, LEFT, 4, 5, "Thermal conductivity of the hot duct in a dual duct system (an alternative to the Hot Duct DT)"
       EDIT, 13103, 13103, 0, 1, SYSTEM, 0,      HOT-DUCT-DT, 0, STD, 900,  80,  23,  50,  2, 3,                  "", LEFT,   -1, 5, 1, LEFT, 4, 5, "Duct air temperature drop when delivering heated air in a dual duct system"
       EDIT, 19229, 19229, 0, 1, SYSTEM, 0, HOTDUCT-ENVIR-DT, 0, STD, 900, 105,  23,  50,  2, 3,                  "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The design differential between the air temperature entering the hot duct, and the duct's environment"

; SAC 11/24/10 - added
; SAC 3/2/11 - moved out of first column & over to second to make room for other new D-2.3 keywords - NOTE: This keyword will be REMOVED once D-2.3 is modified to allow for multiple supply plenums per system
      LABEL,    "Underfloor Air Distribution", STD, LEFT, 385, 145, 1, 0, 0, 655, 0, 3
      COMBO, 19233, 19233, 0, 1, SYSTEM, 0,    SUPPLY-PLENUM, 0, STD, 505, 165, 360, 150, 19, 3,    "Supply Plenum:", LEFT, -105, 5, 0, LEFT, 4, 5, "The underfloor plenum used to supply air to all zones of this system"

; SAC 11/24/10 - shifted 45 pixels right to align w/ compliance ctrls below & shifted 1 row up to accommodate HUMIDITY-REF-T control
      LABEL,    "Humidity Control", STD, LEFT, 740, 235, 1, 0, 0, 1005, 13157, 3
       EDIT, 13157, 13471, 0, 1, SYSTEM, 0,     MAX-HUMIDITY, 0, STD, 885, 255,  23,  50,  1, 3,     "Maximum Humidity:", LEFT, -130, 5, 1, LEFT, 4, 5, "Highest allowable relative humidity in the return air (from all zones served by the system)"
       EDIT, 13158, 13484, 0, 1, SYSTEM, 0,     MIN-HUMIDITY, 0, STD, 885, 280,  23,  50,  1, 3,     "Minimum Humidity:", LEFT, -130, 5, 1, LEFT, 4, 5, "Lowest allowable relative humidity in the return air (from all zones served by the system)"
       EDIT, 19230, 19230, 0, 1, SYSTEM, 0,   HUMIDITY-REF-T, 0, STD, 885, 305,  23,  50,  1, 3,       "Humidity Ref T:", LEFT, -130, 5, 1, LEFT, 4, 5, "The temperature at which the relative humidity MAX-HUMIDITY or the MIN-HUMIDITY is defined"
      COMBO, 13159, 13159, 0, 1, SYSTEM, 0,  HUMIDIFIER-TYPE, 0, STD, 885, 330, 180, 120, 19, 3,      "Humidifier Type:", LEFT, -130, 5, 0, LEFT, 4, 5, "The heat source for humidification in the central air distribution system"
      COMBO, 14532, 14532, 0, 1, SYSTEM, 0,   HUMIDIFIER-LOC, 0, STD, 885, 355, 100, 120, 19, 3,  "Humidifier Location:", LEFT, -130, 5, 0, LEFT, 4, 5, "The location of supply air humidifier"
; DEM 11/28/16 - new keywords used by DOAS
       EDIT, 19483, 19483, 0, 1, SYSTEM, 0,     MAX-DEWPOINT, 0, STD, 885, 380,  23,  50,  1, 3,     "Maximum Dewpoint:", LEFT, -130, 5, 1, LEFT, 4, 5, "Highest allowable dewpoint in the supply air for humidity control"
       EDIT, 19484, 19484, 0, 1, SYSTEM, 0,     MIN-DEWPOINT, 0, STD, 885, 405,  23,  50,  1, 3,     "Minimum Dewpoint:", LEFT, -130, 5, 1, LEFT, 4, 5, "Lowest allowable dewpoint in the supply air for humidity control"

;      LABEL,    "Water Loop Limits", STD, LEFT, 300, 188, 1, 0, 0, 0, 0, 3
;       EDIT, 13110, 13110, 0, 1, SYSTEM, 0,     MIN-FLUID-T, 0, STD, 400, 210,  23,  40,  1, 3,     "Min Fluid T:", LEFT, -100, 5, 1, LEFT, 4, 5, ""
;       EDIT, 13111, 13111, 0, 1, SYSTEM, 0,     MAX-FLUID-T, 0, STD, 400, 235,  23,  40,  1, 3,     "Max Fluid T:", LEFT, -100, 5, 1, LEFT, 4, 5, ""

; AFR 8/13/09 - added      SAC 8/25/09 - minor re-positioning
; SAC 3/2/11 - Shifted leftmost labels to sit above those in second column to allow for several new controls in the first column of dialog box
      LABEL, "Compliance Settings (references)", STD, LEFT, 370, 390, 1, 0, 0, 675, 0, 6
      LABEL, "Heating Source:",         STD, LEFT,  384, 410, 1, 0, 0,   0, 0, 6
      LABEL, "System Type Exception:",  STD, LEFT,  384, 430, 1, 0, 0,   0, 0, 6
      LABEL, "Economizer Exception:",   STD, LEFT,  384, 450, 1, 0, 0,   0, 0, 6
      LABEL, "ERV Exception:",          STD, LEFT,  384, 470, 1, 0, 0,   0, 0, 6

      STATIC, 1, SYSTEM, 0, C-HTG-SYS-CLASS,  0, 0, 0, 675, 410, -1, STD, RIGHT, "",  "", 0, 6
      STATIC, 1, SYSTEM, 0, C-SYS-EXCEPTION1, 0, 0, 0, 675, 430, -1, STD, RIGHT, "",  "", 0, 6
      STATIC, 1, SYSTEM, 0, C-SYS-EXCEPTION2, 0, 0, 0, 675, 450, -1, STD, RIGHT, "",  "", 0, 6
      STATIC, 1, SYSTEM, 0, C-SYS-EXCEPTION3, 0, 0, 0, 675, 470, -1, STD, RIGHT, "",  "", 0, 6


    ;*****************************************
    ; Fans 
    ;*****************************************
    TABPAGE, 3053, 10239, 1, 3, NOTIMP, "  Fans  "
    
       SUBTABPAGE, 3171, 29047, 1, 3, "   Fan Power and Control   "

         LABEL,           "Design", STD, CENTER, 125,  33, 1, 0, 0, 0, 0, 3
         LABEL,           "kW/cfm", STD, CENTER, 125,  49, 1, 0, 0, 0, 0, 3
         
; SAC 11/23/10 - removed          
;         LABEL,          "Delta T", STD, CENTER, 205,  33, 1, 0, 0, 0, 0, 3
;         LABEL,               "°F", STD, CENTER, 205,  49, 1, 0, 0, 0, 0, 3
          
         LABEL,           "Static", STD, CENTER, 205,  33, 1, 0, 0, 0, 0, 3
         LABEL,            "in WG", STD, CENTER, 205,  49, 1, 0, 0, 0, 0, 3
         
; SAC 11/23/10 - added         
         LABEL,      "Motor Class", STD, CENTER, 290,  49, 1, 0, 0, 0, 0, 3
         
; SAC 11/23/10 - removed          
;         LABEL,          "Tot Eff", STD, CENTER, 355,  33, 1, 0, 0, 0, 0, 3
;         LABEL,             "Frac", STD, CENTER, 355,  49, 1, 0, 0, 0, 0, 3

; SAC 11/23/10 - added         
         LABEL,        "Motor Eff", STD, CENTER, 370,  33, 1, 0, 0, 0, 0, 3
         LABEL,             "Frac", STD, CENTER, 370,  49, 1, 0, 0, 0, 0, 3
         
         LABEL,         "Mech Eff", STD, CENTER, 435,  33, 1, 0, 0, 0, 0, 3
         LABEL,             "Frac", STD, CENTER, 435,  49, 1, 0, 0, 0, 0, 3
         
         LABEL, "Fan EIR = f(PLR)", STD, CENTER, 555,  49, 1, 0, 0, 0, 0, 3
         
        CASE, SYSTEM, 0, TYPE, -1, =, 3, 3, 4, 20     
        ;Multizone, Dual Duct, Packaged Multizone
          CASE,  SYSTEM,  0, DDS-TYPE,  -1,  =, 1, 2
          ;Dual fan case
            LABEL, "Fan Power Parameters for Dual-Fan dual-duct or multizone systems", STD, LEFT, 20,  15, 1, 0, 0, 945, 0, 3
            LABEL, "Cooling:", STD, LEFT, 35,  70, 1, 0, 0, 0, 0, 3
            LABEL, "Heating:", STD, LEFT, 35,  95, 1, 0, 0, 0, 0, 3
            LABEL,  "Return:", STD, LEFT, 35, 120, 1, 0, 0, 0, 0, 3
            LABEL, "Cooling:", STD, LEFT, 35, 199, 1, 0, 0, 0, 0, 3
            LABEL, "Heating:", STD, LEFT, 35, 224, 1, 0, 0, 0, 0, 3
            LABEL,  "Return:", STD, LEFT, 35, 249, 1, 0, 0, 0, 0, 3
            LABEL, "Exhaust:", STD, LEFT, 35, 274, 1, 0, 0, 0, 0, 3
; AFR 7/22/09 - compliance    - SAC 8/25/09 - minor re-positioning
            LABEL, "Cooling:", STD, LEFT, 35, 369, 1, 0, 0, 0, 0, 7
            LABEL, "Heating:", STD, LEFT, 35, 394, 1, 0, 0, 0, 0, 7
            LABEL,  "Return:", STD, LEFT, 35, 419, 1, 0, 0, 0, 0, 7
;; AFR 7/22/09 - only allow these control when DSS-TYPE = 2.
;            EDIT, 17860, 17860, 0, 1, SYSTEM, 0, C-HFAN-TOT-NM-HP, 0, STD, 656,  90,  23,  60,  1, 1,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total heating fan nominal (nameplate) motor horsepower for all identical units"
;            EDIT, 17861, 17861, 0, 1, SYSTEM, 0,   C-HFAN-TOT-BHP, 0, STD, 731,  90,  23,  60,  2, 1,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total heating fan brake motor brake horsepower for all identical units"
;            EDIT, 17862, 17862, 0, 1, SYSTEM, 0,   C-HFAN-MTR-EFF, 0, STD, 806,  90,  23,  60,  3, 1,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The efficiency of the heating fan motor"
;            EDIT, 17863, 17863, 0, 1, SYSTEM, 0, C-HFAN-DRIVE-EFF, 0, STD, 881,  90,  23,  60,  3, 1,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The efficiency of the heating fan drive"
;           COMBO, 17856, 17856, 0, 1, SYSTEM, 0,      C-HFAN-TYPE, 0, STD, 656, 219, 300, 140, 19, 1,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The type or flow control of the heating fan"
;            EDIT, 17855, 17855, 0, 1, SYSTEM, 0,       C-HFAN-QTY, 0, STD,  95, 389,  23,  40,  0, 1,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total number of heating fans for all identical units"
;           COMBO, 17857, 17857, 0, 1, SYSTEM, 0,  C-HFAN-MTR-TYPE, 0, STD, 150, 389, 300, 200, 19, 1,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The category describing the heating fan motor efficiency"
;           COMBO, 17858, 17858, 0, 1, SYSTEM, 0,   C-HFAN-MTR-SPD, 0, STD, 365, 389, 300,  90, 19, 1,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The synchronous speed of the heating fan motor"
;           COMBO, 17859, 17859, 0, 1, SYSTEM, 0,  C-HFAB-MTR-ENCL, 0, STD, 470, 389, 300,  90, 19, 1,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The type of enclosure for the heating fan motor"
        CHECKBOX, 17864, 17864, 0, 1, SYSTEM, 0,  C-HF-FILTRATION, 0, STD, 595, 389,  18,  20,     7,     "", LEFT,                         "Checked if specialized filtration exceeds 1 in. static pressure drop"
            EDIT, 17866, 17866, 0, 1, SYSTEM, 0,      C-HF-TOT-SP, 0, STD, 650, 389,  23,  80,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total static pressure of the heating air system"
            EDIT, 17865, 17865, 0, 1, SYSTEM, 0,     C-HF-FILT-SP, 0, STD, 745, 389,  23,  80,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The pressure drop through the specialized heating filtration equipment"
            
          ENDCASE 
          CASE,  SYSTEM,  0, DDS-TYPE,  -1,  <, 1, 2
          ;Single fan case
            LABEL, "Fan Power Parameters for Single-Fan dual-duct or multizone systems", STD, LEFT, 20,  15, 1, 0, 0, 945, 0, 3
            LABEL,  "Supply:", STD, LEFT, 35,  70, 1, 0, 0, 0, 0, 3
            LABEL,  "Unused:", STD, LEFT, 35,  95, 1, 0, 0, 0, 0, 3
            LABEL,  "Return:", STD, LEFT, 35, 120, 1, 0, 0, 0, 0, 3
            LABEL, "Cooling:", STD, LEFT, 35, 199, 1, 0, 0, 0, 0, 3
            LABEL,  "Unused:", STD, LEFT, 35, 224, 1, 0, 0, 0, 0, 3
            LABEL,  "Return:", STD, LEFT, 35, 249, 1, 0, 0, 0, 0, 3
            LABEL, "Exhaust:", STD, LEFT, 35, 274, 1, 0, 0, 0, 0, 3
; AFR 7/22/09 - compliance    - SAC 8/25/09 - minor re-positioning
            LABEL, "Cooling:", STD, LEFT, 35, 369, 1, 0, 0, 0, 0, 7
            LABEL,  "Unused:", STD, LEFT, 35, 394, 1, 0, 0, 0, 0, 7
            LABEL,  "Return:", STD, LEFT, 35, 419, 1, 0, 0, 0, 0, 7
          ENDCASE 
        ENDCASE 
        CASE, SYSTEM, 0, TYPE, -1, =, 29, 1,2,5,6,7,8,9,10,11,12,13,14,15,16,17,18,19,21,22,23,24,25,26,27,28,29,30,31,32
        ;everthing except Multizone, Dual Duct, Packaged Multizone
          LABEL, "Fan Power Parameters for single-duct systems", STD, LEFT, 20,  15, 1, 0, 0, 945, 0, 3
          LABEL,  "Supply:", STD, LEFT, 35,  70, 1, 0, 0, 0, 0, 3
          LABEL,  "Unused:", STD, LEFT, 35,  95, 1, 0, 0, 0, 0, 3
          LABEL,  "Return:", STD, LEFT, 35, 120, 1, 0, 0, 0, 0, 3
          LABEL, "Cooling:", STD, LEFT, 35, 199, 1, 0, 0, 0, 0, 3
          LABEL,  "Unused:", STD, LEFT, 35, 224, 1, 0, 0, 0, 0, 3
          LABEL,  "Return:", STD, LEFT, 35, 249, 1, 0, 0, 0, 0, 3
          LABEL, "Exhaust:", STD, LEFT, 35, 274, 1, 0, 0, 0, 0, 3
; AFR 7/22/09 - compliance    - SAC 8/25/09 - minor re-positioning
          LABEL, "Cooling:", STD, LEFT, 35, 369, 1, 0, 0, 0, 0, 7
          LABEL,  "Unused:", STD, LEFT, 35, 394, 1, 0, 0, 0, 0, 7
          LABEL,  "Return:", STD, LEFT, 35, 419, 1, 0, 0, 0, 0, 7
        ENDCASE 

          EDIT, 13065, 12306, 0, 1, SYSTEM, 0,   SUPPLY-KW/FLOW, 0, STD,  90,  65,  23,  70,  6, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Cooling Design kW/CFM
          EDIT, 13066, 13066, 0, 1, SYSTEM, 0,  HSUPPLY-KW/FLOW, 0, STD,  90,  90,  23,  70,  6, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Full load power consumption of the heating supply fan, per unit heating supply air per hour"
          EDIT, 13067, 12307, 0, 1, SYSTEM, 0,   RETURN-KW/FLOW, 0, STD,  90, 115,  23,  70,  6, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Return  Design kW/CFM

; SAC 11/23/10 - removed          
;          EDIT, 13068, 13430, 0, 1, SYSTEM, 0,   SUPPLY-DELTA-T, 0, STD, 175,  65,  23,  60,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Temp rise in the air stream across the supply fan (cooling fan for dual duct dual fan systems)"
;          EDIT, 13069, 13431, 0, 1, SYSTEM, 0,  HSUPPLY-DELTA-T, 0, STD, 175,  90,  23,  60,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "The temperature rise in the air stream across the heating supply fan"
;          EDIT, 13070, 13432, 0, 1, SYSTEM, 0,   RETURN-DELTA-T, 0, STD, 175, 115,  23,  60,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Temperature rise in the air stream across the return air fan"
                                                                                                         
          EDIT, 13071, 13433, 0, 1, SYSTEM, 0,    SUPPLY-STATIC, 0, STD, 175,  65,  23,  60,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Total increase in air pressure across the supply air fan (at the design flow rate)"
          EDIT, 13072, 13434, 0, 1, SYSTEM, 0,   HSUPPLY-STATIC, 0, STD, 175,  90,  23,  60,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Total increase in air pressure across the heating supply air fan (for dual duct systems)"
          EDIT, 13073, 13435, 0, 1, SYSTEM, 0,    RETURN-STATIC, 0, STD, 175, 115,  23,  60,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Total increase in air pressure across the return air fan (at the design flow rate)"

; SAC 11/23/10 - added
         COMBO, 19212, 19212, 0, 1, SYSTEM, 0,  SUPPLY-MTR-CLASS, 0, STD, 250,  65, 200,  80, 19, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Specifies the motor class (efficiency) of the HVAC supply fans"
; SAC 2/23/11 - added
         COMBO, 19321, 19321, 0, 1, SYSTEM, 0,  HSUPPLY-MTR-CLAS, 0, STD, 250,  90, 200,  80, 19, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Specifies the motor class (efficiency) of the HVAC heating supply fans"
         COMBO, 19322, 19322, 0, 1, SYSTEM, 0,  RETURN-MTR-CLASS, 0, STD, 250, 115, 200,  80, 19, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Specifies the motor class (efficiency) of the HVAC return fans"
          
; SAC 11/23/10 - removed          
;          EDIT, 13094, 13436, 0, 1, SYSTEM, 0,       SUPPLY-EFF, 0, STD, 325,  65,  23,  60,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Overall efficiency of the supply air fan and motor (at the design flow rate)"
;          EDIT, 13112, 13437, 0, 1, SYSTEM, 0,      HSUPPLY-EFF, 0, STD, 325,  90,  23,  60,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Overall efficiency of the heating supply air fan and motor (at the design flow rate)"
;          EDIT, 13113, 13438, 0, 1, SYSTEM, 0,       RETURN-EFF, 0, STD, 325, 115,  23,  60,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Overall efficiency of the return air fan and motor (at the design flow rate)"

; SAC 11/23/10 - added
          EDIT, 19209, 19209, 0, 1, SYSTEM, 0,   SUPPLY-MTR-EFF, 0, STD, 345,  65,  23,  50,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Efficiency of the supply fan motor"
          EDIT, 19210, 19210, 0, 1, SYSTEM, 0,  HSUPPLY-MTR-EFF, 0, STD, 345,  90,  23,  50,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Efficiency of heating supply fan motor"
          EDIT, 19211, 19211, 0, 1, SYSTEM, 0,   RETURN-MTR-EFF, 0, STD, 345, 115,  23,  50,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Efficiency of return fan motor"
          
          EDIT, 13117, 13117, 0, 1, SYSTEM, 0,  SUPPLY-MECH-EFF, 0, STD, 410,  65,  23,  50,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Mechanical efficiency of the supply fan when the motor is located outside the air stream"
          EDIT, 12919, 12919, 0, 1, SYSTEM, 0, HSUPPLY-MECH-EFF, 0, STD, 410,  90,  23,  50,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Mechanical efficiency of heating supply fan when the motor is located outside the air stream"
; SAC 11/23/10 - added
          EDIT, 19208, 19208, 0, 1, SYSTEM, 0,  RETURN-MECH-EFF, 0, STD, 410, 115,  23,  50,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Mechanical efficiency of return fan when the motor is located outside the air stream"
                                                                                                                                                                                                                                          
         COMBO, 13095, 13441, 0, 1, SYSTEM, 0,     FAN-EIR-FPLR, 0, STD, 475,  65, 200, 165, 19, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Cubic Curve Fit: Electric Input Ratio as a function of the fan's part load ratio"
         COMBO, 13096, 13442, 0, 1, SYSTEM, 0,    HFAN-EIR-FPLR, 0, STD, 475,  90, 200, 165, 19, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Cubic Curve Fit: Electric Input Ratio as a function of the fan's part load ratio"
         COMBO, 13105, 13443, 0, 1, SYSTEM, 0,  RETURN-EIR-FPLR, 0, STD, 475, 115, 200, 165, 19, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Cubic Curve Fit: Electric Input Ratio as a function of the fan's part load ratio"


         LABEL, "Fan Control and Placement", STD, LEFT, 20, 160, 1, 0, 0, 795, 0, 3
         
         LABEL,   "Fan Schedules", STD, CENTER, 165, 178, 1, 0, 0, 0, 0, 3
         LABEL,     "Fan Control", STD, CENTER, 325, 178, 1, 0, 0, 0, 0, 3
         LABEL,   "Fan Placement", STD, CENTER, 462, 178, 1, 0, 0, 0, 0, 3
         LABEL, "Motor Placement", STD, CENTER, 585, 178, 1, 0, 0, 0, 0, 3
         
;        LABEL, "Cooling:", STD, LEFT, 18, 250, 1, 0, 0, 0, 0, 3
;        LABEL, "Heating:", STD, LEFT, 18, 275, 1, 0, 0, 0, 0, 3
;        LABEL,  "Return:", STD, LEFT, 18, 300, 1, 0, 0, 0, 0, 3
;        LABEL, "Exhaust:", STD, LEFT, 18, 325, 1, 0, 0, 0, 0, 3

         COMBO, 12938, 12938, 0, 1, SYSTEM, 0,     FAN-SCHEDULE, 0, STD,  90, 194, 300, 155, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Cooling Fan Schedules
         COMBO, 12939, 12939, 0, 1, SYSTEM, 0,    HFAN-SCHEDULE, 0, STD,  90, 219, 300, 155, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Heating Fan Schedules
         COMBO, 12940, 12940, 0, 1, SYSTEM, 0,  EXHAUST-FAN-SCH, 0, STD,  90, 269, 300, 155, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "Specifies when this system's central exhaust fans can operate"
         
         COMBO, 12941, 12941, 0, 1, SYSTEM, 0,      FAN-CONTROL, 0, STD, 260, 194, 180, 135, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "Specifies the type of flow reduction or control methods to be simulated"
         COMBO, 12942, 12942, 0, 1, SYSTEM, 0,     HFAN-CONTROL, 0, STD, 260, 219, 180, 135, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "Specifies the type of flow reduction or control methods to be simulated"
         COMBO, 12943, 12943, 0, 1, SYSTEM, 0, RETURN-FAN-CONTR, 0, STD, 260, 244, 180, 135, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "Specifies the kind of flow reduction or control methods to be simulated"
         
         COMBO, 12966, 12966, 0, 1, SYSTEM, 0,    FAN-PLACEMENT, 0, STD, 410, 194,  70, 110, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "Whether supply fan is before or after the coils (applies to cooling fan for dual duct systems)"
         COMBO, 12971, 12971, 0, 1, SYSTEM, 0,   HFAN-PLACEMENT, 0, STD, 410, 219,  70, 110, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "Whether the heating supply fan is before or after the heating coils (in dual duct systems)"
         COMBO, 12990, 12990, 0, 1, SYSTEM, 0,   RETURN-FAN-LOC, 0, STD, 410, 244, 100, 110, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "Location of the return fan (if present)"
         
         COMBO, 13048, 13048, 0, 1, SYSTEM, 0,  MOTOR-PLACEMENT, 0, STD, 535, 194,  70, 105, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "Whether the supply and return fan motor heat is added to the airstream"
         COMBO, 13049, 13049, 0, 1, SYSTEM, 0, HMOTOR-PLACEMENT, 0, STD, 535, 219,  70, 105, 19, 3,                "", LEFT, -2, 5, 0, LEFT, 4, 5, "Whether the heating supply fan motor heat is added to the airstream"

; AFR 7/22/09 - Compliance data labels.
; top section compliance labels         
         LABEL, "Tot Motor",                    STD, CENTER, 686,  33, 1, 0, 0, 0, 0, 7
         LABEL, "Nom HP",                       STD, CENTER, 686,  49, 1, 0, 0, 0, 0, 7
         
         LABEL, "Tot Motor",                    STD, CENTER, 763,  33, 1, 0, 0, 0, 0, 7
         LABEL, "Brake HP",                     STD, CENTER, 763,  49, 1, 0, 0, 0, 0, 7
         
         LABEL, "Avg. Motor",                   STD, CENTER, 836,  33, 1, 0, 0, 0, 0, 7
         LABEL, "Eff Frac",                     STD, CENTER, 836,  49, 1, 0, 0, 0, 0, 7
         
         LABEL, "Motor Drive",                  STD, CENTER, 912,  33, 1, 0, 0, 0, 0, 7
         LABEL, "Eff Frac",                     STD, CENTER, 912,  49, 1, 0, 0, 0, 0, 7

; middle section compliance labels
         LABEL, "Compliance Fan Type",          STD, CENTER, 723, 178, 1, 0, 0, 0, 0, 7
         
; bottom section compliance labels         
         LABEL, "Additional Compliance Inputs", STD, LEFT, 20, 314, 1, 0, 0, 825, 0, 7
         
         LABEL, "Fan Qty",                      STD, CENTER, 115, 348, 1, 0, 0, 0, 0, 7
         
         LABEL, "Motor Efficiency Category",    STD, CENTER, 255, 348, 1, 0, 0, 0, 0, 7
         
         LABEL, "Motor Synch",                  STD, CENTER, 410, 332, 1, 0, 0, 0, 0, 7
         LABEL, "Speed",                        STD, CENTER, 410, 348, 1, 0, 0, 0, 0, 7
         
         LABEL, "Motor",                        STD, CENTER, 515, 332, 1, 0, 0, 0, 0, 7
         LABEL, "Enclosure",                    STD, CENTER, 515, 348, 1, 0, 0, 0, 0, 7

         LABEL, "Special",                      STD, CENTER, 600, 332, 1, 0, 0, 0, 0, 7
         LABEL, "Filtration",                   STD, CENTER, 600, 348, 1, 0, 0, 0, 0, 7
         
         LABEL, "Total Static",                 STD, CENTER, 690, 332, 1, 0, 0, 0, 0, 7
         LABEL, "in WG",                        STD, CENTER, 690, 348, 1, 0, 0, 0, 0, 7
         
         LABEL, "Filtration Static",            STD, CENTER, 785, 332, 1, 0, 0, 0, 0, 7
         LABEL, "in WG",                        STD, CENTER, 785, 348, 1, 0, 0, 0, 0, 7
         
; AFR 7/22/09 - Compliance data controls
; top section compliance controls          
          EDIT, 15525, 15525, 0, 1, SYSTEM, 0,  C-SF-TOT-NOM-HP, 0, STD, 656,  65,  23,  60,  1, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total supply fan nominal (nameplate) motor horsepower for all identical units"
          EDIT, 15526, 15526, 0, 1, SYSTEM, 0,     C-SF-TOT-BHP, 0, STD, 731,  65,  23,  60,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total supply fan brake motor brake horsepower for all identical units"
          EDIT, 15527, 15527, 0, 1, SYSTEM, 0,   C-SF-MOTOR-EFF, 0, STD, 806,  65,  23,  60,  3, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The efficiency of the supply fan motor"
          EDIT, 15528, 15528, 0, 1, SYSTEM, 0,   C-SF-DRIVE-EFF, 0, STD, 881,  65,  23,  60,  3, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The efficiency of the supply fan drive"
          
          EDIT, 17860, 17860, 0, 1, SYSTEM, 0, C-HFAN-TOT-NM-HP, 0, STD, 656,  90,  23,  60,  1, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total heating fan nominal (nameplate) motor horsepower for all identical units"
          EDIT, 17861, 17861, 0, 1, SYSTEM, 0,   C-HFAN-TOT-BHP, 0, STD, 731,  90,  23,  60,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total heating fan brake motor brake horsepower for all identical units"
          EDIT, 17862, 17862, 0, 1, SYSTEM, 0,   C-HFAN-MTR-EFF, 0, STD, 806,  90,  23,  60,  3, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The efficiency of the heating fan motor"
          EDIT, 17863, 17863, 0, 1, SYSTEM, 0, C-HFAN-DRIVE-EFF, 0, STD, 881,  90,  23,  60,  3, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The efficiency of the heating fan drive"
          
          EDIT, 15537, 15537, 0, 1, SYSTEM, 0,  C-RF-TOT-NOM-HP, 0, STD, 656, 115,  23,  60,  1, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total return fan nominal (nameplate) motor horsepower for all identical units"
          EDIT, 15538, 15538, 0, 1, SYSTEM, 0,     C-RF-TOT-BHP, 0, STD, 731, 115,  23,  60,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total return fan brake motor brake horsepower for all identical units"
          EDIT, 15539, 15539, 0, 1, SYSTEM, 0,   C-RF-MOTOR-EFF, 0, STD, 806, 115,  23,  60,  3, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The efficiency of the return fan motor"
          EDIT, 15540, 15540, 0, 1, SYSTEM, 0,   C-RF-DRIVE-EFF, 0, STD, 881, 115,  23,  60,  3, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The efficiency of the return fan drive"

; middle section compliance controls          
         COMBO, 15522, 15522, 0, 1, SYSTEM, 0,  C-SUPP-FAN-TYPE, 0, STD, 656, 194, 300, 140, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The type or flow control of the supply fan"
         COMBO, 17856, 17856, 0, 1, SYSTEM, 0,      C-HFAN-TYPE, 0, STD, 656, 219, 300, 140, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The type or flow control of the heating fan"
         COMBO, 15534, 15534, 0, 1, SYSTEM, 0,   C-RET-FAN-TYPE, 0, STD, 656, 244, 300, 140, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The type or flow control of the return fan"

; bottom section compliance controls
          EDIT, 15521, 15521, 0, 1, SYSTEM, 0,    C-SUP-FAN-QTY, 0, STD,  95, 364,  23,  40,  0, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total number of supply fans for all identical units"
         COMBO, 15524, 15524, 0, 1, SYSTEM, 0,    C-SF-MTR-TYPE, 0, STD, 150, 364, 300, 200, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The category describing the supply fan motor efficiency"
         COMBO, 15523, 15523, 0, 1, SYSTEM, 0, C-SF-MTR-SNC-SPD, 0, STD, 365, 364, 300,  90, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The synchronous speed of the supply fan motor"
         COMBO, 17501, 17501, 0, 1, SYSTEM, 0,    C-SF-MTR-ENCL, 0, STD, 470, 364, 300,  90, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The type of enclosure for the supply fan motor"
; DEM 10/26/12 new keyword for motor subtype to identify T24 level
         COMBO, 17201, 17201, 0, 1, SYSTEM, 0, C-SFAN-MOTOR-SUB, 0, STD, 575, 364, 300, 170, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "Motor phase and subtype classification"
      CHECKBOX, 15529, 15529, 0, 1, SYSTEM, 0,  C-SF-FILTRATION, 0, STD, 773, 364,  18,  20,     7,     "", LEFT,                       "Checked if specialized filtration exceeds 1 in. static pressure drop"
          EDIT, 15531, 15531, 0, 1, SYSTEM, 0,      C-SF-TOT-SP, 0, STD, 815, 364,  23,  80,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total static pressure of the supply air system"
          EDIT, 15530, 15530, 0, 1, SYSTEM, 0,     C-SF-FILT-SP, 0, STD, 910, 364,  23,  80,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The pressure drop through the specialized supply filtration equipment"

          EDIT, 17855, 17855, 0, 1, SYSTEM, 0,       C-HFAN-QTY, 0, STD,  95, 389,  23,  40,  0, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total number of heating fans for all identical units"
         COMBO, 17857, 17857, 0, 1, SYSTEM, 0,  C-HFAN-MTR-TYPE, 0, STD, 150, 389, 300, 200, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The category describing the heating fan motor efficiency"
         COMBO, 17858, 17858, 0, 1, SYSTEM, 0,   C-HFAN-MTR-SPD, 0, STD, 365, 389, 300,  90, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The synchronous speed of the heating fan motor"
         COMBO, 17859, 17859, 0, 1, SYSTEM, 0,  C-HFAB-MTR-ENCL, 0, STD, 470, 389, 300,  90, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The type of enclosure for the heating fan motor"
         COMBO, 17202, 17201, 0, 1, SYSTEM, 0, C-HFAN-MOTOR-SUB, 0, STD, 575, 389, 300, 170, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "Motor phase and subtype classification"
      CHECKBOX, 17864, 17864, 0, 1, SYSTEM, 0,  C-HF-FILTRATION, 0, STD, 773, 389,  18,  20,     7,     "", LEFT,                         "Checked if specialized filtration exceeds 1 in. static pressure drop"
          EDIT, 17866, 17866, 0, 1, SYSTEM, 0,      C-HF-TOT-SP, 0, STD, 815, 389,  23,  80,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total static pressure of the heating air system"
          EDIT, 17865, 17865, 0, 1, SYSTEM, 0,     C-HF-FILT-SP, 0, STD, 910, 389,  23,  80,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The pressure drop through the specialized heating filtration equipment"


          EDIT, 15533, 15533, 0, 1, SYSTEM, 0,    C-RET-FAN-QTY, 0, STD,  95, 414,  23,  40,  0, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total number of return fans for all identical units"
         COMBO, 15535, 15535, 0, 1, SYSTEM, 0,    C-RF-MTR-TYPE, 0, STD, 150, 414, 300, 200, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The category describing the return fan motor efficiency"
         COMBO, 15536, 15536, 0, 1, SYSTEM, 0, C-RF-MTR-SNC-SPD, 0, STD, 365, 414, 300,  90, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The synchronous speed of the return fan motor"
         COMBO, 17502, 17502, 0, 1, SYSTEM, 0,    C-RF-MTR-ENCL, 0, STD, 470, 414, 300,  90, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The type of enclosure for the return fan motor"
         COMBO, 17203, 17201, 0, 1, SYSTEM, 0, C-RFAN-MOTOR-SUB, 0, STD, 575, 414, 300, 170, 19, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "Motor phase and subtype classification"
      CHECKBOX, 15541, 15541, 0, 1, SYSTEM, 0,  C-RF-FILTRATION, 0, STD, 773, 414,  18,  20,     7,     "", LEFT,                       "Checked if specialized filtration exceeds 1 in. static pressure drop"
          EDIT, 15543, 15543, 0, 1, SYSTEM, 0,      C-RF-TOT-SP, 0, STD, 815, 414,  23,  80,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The total static pressure of the return air system"
          EDIT, 15542, 15542, 0, 1, SYSTEM, 0,     C-RF-FILT-SP, 0, STD, 910, 414,  23,  80,  2, 7,     "", LEFT, -1, 5, 0, LEFT, 4, 5, "The pressure drop through the specialized return filtration equipment"


         

;////////////////////////////////////////////////////////////////////




       SUBTABPAGE, 3172, 29046, 1, 3, "   Flow Parameters   "

         LABEL,   "Design", STD, CENTER, 213, 33, 1, 0, 0, 0, 0, 3
         LABEL,      "cfm", STD, CENTER, 213, 49, 1, 0, 0, 0, 0, 3
      
         LABEL, "Min Flow", STD, CENTER, 308, 33, 1, 0, 0, 0, 0, 3
         LABEL,  "cfm/ft2", STD, CENTER, 308, 49, 1, 0, 0, 0, 0, 3
         
         LABEL, "Min Flow", STD, CENTER, 403, 33, 1, 0, 0, 0, 0, 3
         LABEL,    "Ratio", STD, CENTER, 403, 49, 1, 0, 0, 0, 0, 3
         
         LABEL, "Max Flow", STD, CENTER, 498, 33, 1, 0, 0, 0, 0, 3    ; SAC 12/11/09 - added
         LABEL,    "Ratio", STD, CENTER, 498, 49, 1, 0, 0, 0, 0, 3
         
         LABEL,  "Min Fan", STD, CENTER, 593, 33, 1, 0, 0, 0, 0, 3
         LABEL,    "Ratio", STD, CENTER, 593, 49, 1, 0, 0, 0, 0, 3
         
         LABEL,  "Max Fan", STD, CENTER, 688, 33, 1, 0, 0, 0, 0, 3
         LABEL,    "Ratio", STD, CENTER, 688, 49, 1, 0, 0, 0, 0, 3
      
        CASE, SYSTEM, 0, TYPE, -1, =, 3, 3, 4, 20     
        ;Multizone, Dual Duct, Packaged Multizone

          CASE,  SYSTEM,  0, DDS-TYPE,  -1,  <, 1, 2
          ;Single fan case
           LABEL, "Flow Parameters for Single-Fan dual-duct or multizone systems", STD, LEFT, 20, 15, 1, 0, 0, 730, 0, 3
           LABEL, "Overall Supply Flow:", STD, LEFT, 35,  70, 1, 0, 0, 0, 0, 3
           LABEL, "Cooling Supply Flow:", STD, LEFT, 35,  95, 1, 0, 0, 0, 0, 3
           LABEL, "Heating Supply Flow:", STD, LEFT, 35, 120, 1, 0, 0, 0, 0, 3
           LABEL, "Return Flow:",         STD, LEFT, 35, 145, 1, 0, 0, 0, 0, 3

           EDIT, 12913, 13424, 0, 1, SYSTEM, 0,      SUPPLY-FLOW, 0, STD, 175,  65,  23,  80,  0, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Cooling Design CFM
;2ndrow    EDIT, 12913, 13424, 0, 1, SYSTEM, 0,      SUPPLY-FLOW, 0, STD, 175,  90,  23,  80,  0, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Cooling Design CFM
;          EDIT, 12914, 13425, 0, 1, SYSTEM, 0,     HSUPPLY-FLOW, 0, STD, 175, 115,  23,  80,  0, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Design air flow rate of the hot air supply fan for the hot duct of a dual-duct dual fan system"
           EDIT, 12915, 13426, 0, 1, SYSTEM, 0,      RETURN-FLOW, 0, STD, 175, 140,  23,  80,  0, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Return  Design CFM
       
           EDIT, 13114, 13439, 0, 1, SYSTEM, 0,    MIN-FLOW/AREA, 0, STD, 270,  65,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum total supply air flow rate per unit floor area (alternative is Min Flow Ratio)"
           EDIT, 12918, 12918, 0, 1, SYSTEM, 0,   CMIN-FLOW/AREA, 0, STD, 270,  90,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum allowable cooling supply air flow rate per square foot of floor area"
           EDIT, 12920, 12920, 0, 1, SYSTEM, 0,   HMIN-FLOW/AREA, 0, STD, 270, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum allowable heating supply air flow rate per square foot of floor area" ;Heating Min Flow CFM
       
           EDIT, 12911, 13440, 0, 1, SYSTEM, 0,   MIN-FLOW-RATIO, 0, STD, 365,  65,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum allowable supply air flow rate (as a fraction of the design flow rate)"
           EDIT, 12921, 12921, 0, 1, SYSTEM, 0,  CMIN-FLOW-RATIO, 0, STD, 365,  90,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "The minimum airflow ratio of the cold duct damper controller" ;Cooling Min Flow Ratio
           EDIT, 12922, 12922, 0, 1, SYSTEM, 0,  HMIN-FLOW-RATIO, 0, STD, 365, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum airflow ratio of the hot duct damper controller (VAV only)" ;Heating Min Flow Ratio
       
           EDIT, 19197, 19197, 0, 1, SYSTEM, 0,  HMAX-FLOW-RATIO, 0, STD, 460, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "The ratio of the maximum (or fixed) heating airflow to the cooling airflow (VAVS and PVAVS only)"    ; SAC 12/11/09

           EDIT, 12923, 12923, 0, 1, SYSTEM, 0,    MIN-FAN-RATIO, 0, STD, 555,  65,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Min allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
;2ndrow    EDIT, 12923, 12923, 0, 1, SYSTEM, 0,    MIN-FAN-RATIO, 0, STD, 555,  90,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Min allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
;          EDIT, 12924, 12924, 0, 1, SYSTEM, 0,   HMIN-FAN-RATIO, 0, STD, 555, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum allowable air flow through heating fan for dual duct systems"
       
           EDIT, 12930, 12930, 0, 1, SYSTEM, 0,    MAX-FAN-RATIO, 0, STD, 650,  65,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Max allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
;2ndrow    EDIT, 12930, 12930, 0, 1, SYSTEM, 0,    MAX-FAN-RATIO, 0, STD, 650,  90,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Max allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
;          EDIT, 12931, 12931, 0, 1, SYSTEM, 0,   HMAX-FAN-RATIO, 0, STD, 650, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Maximum allowable air flow through heating fan for dual duct systems"
          ENDCASE     

          CASE,  SYSTEM,  0, DDS-TYPE,  -1,  =, 1, 2
          ;Dual fan case
           LABEL, "Flow Parameters for Dual-Fan dual-duct or multizone systems", STD, LEFT, 20, 15, 1, 0, 0, 730, 0, 3
           LABEL, "Overall Supply Flow:", STD, LEFT, 35,  70, 1, 0, 0, 0, 0, 3
           LABEL, "Cooling Supply Flow:", STD, LEFT, 35,  95, 1, 0, 0, 0, 0, 3
           LABEL, "Heating Supply Flow:", STD, LEFT, 35, 120, 1, 0, 0, 0, 0, 3
           LABEL, "Return Flow:",         STD, LEFT, 35, 145, 1, 0, 0, 0, 0, 3

;1strow    EDIT, 14580, 13424, 0, 1, SYSTEM, 0,      SUPPLY-FLOW, 0, STD, 175,  65,  23,  80,  0, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Cooling Design CFM
           EDIT, 14580, 13424, 0, 1, SYSTEM, 0,      SUPPLY-FLOW, 0, STD, 175,  90,  23,  80,  0, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Cooling Design CFM
           EDIT, 12914, 13425, 0, 1, SYSTEM, 0,     HSUPPLY-FLOW, 0, STD, 175, 115,  23,  80,  0, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Design air flow rate of the hot air supply fan for the hot duct of a dual-duct dual fan system"
           EDIT, 14581, 13426, 0, 1, SYSTEM, 0,      RETURN-FLOW, 0, STD, 175, 140,  23,  80,  0, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" ;Return  Design CFM
       
           EDIT, 14579, 13439, 0, 1, SYSTEM, 0,    MIN-FLOW/AREA, 0, STD, 270,  65,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum total supply air flow rate per square foot of floor area (alternative is Min Flow Ratio)"
           EDIT, 14582, 12918, 0, 1, SYSTEM, 0,   CMIN-FLOW/AREA, 0, STD, 270,  90,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum allowable cooling supply air flow rate per square foot of floor area" ;Cooling Min Flow CFM
           EDIT, 14583, 12920, 0, 1, SYSTEM, 0,   HMIN-FLOW/AREA, 0, STD, 270, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum allowable heating supply air flow rate per square foot of floor area" ;Heating Min Flow CFM
       
           EDIT, 14584, 13440, 0, 1, SYSTEM, 0,   MIN-FLOW-RATIO, 0, STD, 365,  65,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum allowable supply air flow rate (as a fraction of the design flow rate)"
           EDIT, 14585, 12921, 0, 1, SYSTEM, 0,  CMIN-FLOW-RATIO, 0, STD, 365,  90,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "The minimum airflow ratio of the cold duct damper controller" ;Cooling Min Flow Ratio
           EDIT, 14586, 12922, 0, 1, SYSTEM, 0,  HMIN-FLOW-RATIO, 0, STD, 365, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum airflow ratio of the hot duct damper controller (VAV only)" ;Heating Min Flow Ratio
       
           EDIT, 19198, 19198, 0, 1, SYSTEM, 0,  HMAX-FLOW-RATIO, 0, STD, 460, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "The ratio of the maximum (or fixed) heating airflow to the cooling airflow (VAVS and PVAVS only)"    ; SAC 12/11/09
       
;1strow    EDIT, 14587, 12923, 0, 1, SYSTEM, 0,    MIN-FAN-RATIO, 0, STD, 555,  65,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Min allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
           EDIT, 14587, 12923, 0, 1, SYSTEM, 0,    MIN-FAN-RATIO, 0, STD, 555,  90,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Min allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
           EDIT, 12924, 12924, 0, 1, SYSTEM, 0,   HMIN-FAN-RATIO, 0, STD, 555, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Minimum allowable air flow through heating fan for dual duct systems"
       
;1strow    EDIT, 14588, 12930, 0, 1, SYSTEM, 0,    MAX-FAN-RATIO, 0, STD, 650,  65,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Max allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
           EDIT, 14588, 12930, 0, 1, SYSTEM, 0,    MAX-FAN-RATIO, 0, STD, 650,  90,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Max allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
           EDIT, 12931, 12931, 0, 1, SYSTEM, 0,   HMAX-FAN-RATIO, 0, STD, 650, 115,  23,  80,  2, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "Maximum allowable air flow through heating fan for dual duct systems"
          ENDCASE     

        ENDCASE     

        CASE, SYSTEM, 0, TYPE, -1, =, 29, 1,2,5,6,7,8,9,10,11,12,13,14,15,16,17,18,19,21,22,23,24,25,26,27,28,29,30,31,32
        ;everthing except Multizone, Dual Duct, Packaged Multizone
          LABEL, "Flow Parameters for single-duct systems", STD, LEFT, 20, 15, 1, 0, 0, 730, 0, 3
          LABEL,       "Supply Flow:", STD, LEFT, 35,  70, 1, 0, 0, 0, 0, 3
;         LABEL,  "Cooling Fan/Flow:", STD, LEFT, 35,  95, 1, 0, 0, 0, 0, 3
          LABEL,      "Heating Mode:", STD, LEFT, 35,  95, 1, 0, 0, 0, 0, 3
          LABEL,       "Return Flow:", STD, LEFT, 35, 120, 1, 0, 0, 0, 0, 3

          EDIT, 14590, 13424, 0, 1, SYSTEM, 0,      SUPPLY-FLOW, 0, STD, 175,  65,  23,  80,  0, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "" ;Cooling Design CFM
;2ndrow   EDIT, 14590, 13424, 0, 1, SYSTEM, 0,      SUPPLY-FLOW, 0, STD, 175,  90,  23,  80,  0, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "" ;Cooling Design CFM
;         EDIT, 12914, 13425, 0, 1, SYSTEM, 0,     HSUPPLY-FLOW, 0, STD, 175, 115,  23,  80,  0, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "" ;Heating Design CFM
          EDIT, 14591, 13426, 0, 1, SYSTEM, 0,      RETURN-FLOW, 0, STD, 175, 115,  23,  80,  0, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "" ;Return  Design CFM
       
          EDIT, 14589, 13439, 0, 1, SYSTEM, 0,    MIN-FLOW/AREA, 0, STD, 270,  65,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Minimum total supply air flow rate per square foot of floor area (alternative is Min Flow Ratio)"
;         EDIT, 12918, 12918, 0, 1, SYSTEM, 0,   CMIN-FLOW/AREA, 0, STD, 270,  90,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Minimum allowable cooling supply air flow rate per square foot of floor area" ;Cooling Min Flow CFM
          EDIT, 14596, 12920, 0, 1, SYSTEM, 0,   HMIN-FLOW/AREA, 0, STD, 270,  90,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Minimum allowable heating supply air flow rate per square foot of floor area" ;Heating Min Flow CFM
       
          EDIT, 14592, 13440, 0, 1, SYSTEM, 0,   MIN-FLOW-RATIO, 0, STD, 365,  65,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Minimum allowable supply air flow rate (as a fraction of the design flow rate)"
;         EDIT, 12921, 12921, 0, 1, SYSTEM, 0,  CMIN-FLOW-RATIO, 0, STD, 365,  90,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "The minimum airflow ratio of the cold duct damper controller" ;Cooling Min Flow Ratio
          EDIT, 14597, 12922, 0, 1, SYSTEM, 0,  HMIN-FLOW-RATIO, 0, STD, 365,  90,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Minimum airflow ratio of the hot duct damper controller (VAV only)" ;Heating Min Flow Ratio
       
          EDIT, 19199, 19199, 0, 1, SYSTEM, 0,  HMAX-FLOW-RATIO, 0, STD, 460,  90,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "The ratio of the maximum (or fixed) heating airflow to the cooling airflow (VAVS and PVAVS only)"    ; SAC 12/11/09
       
          EDIT, 14593, 12923, 0, 1, SYSTEM, 0,    MIN-FAN-RATIO, 0, STD, 555,  65,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Min allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
;2ndrow   EDIT, 14593, 12923, 0, 1, SYSTEM, 0,    MIN-FAN-RATIO, 0, STD, 555,  90,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Min allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
;         EDIT, 12924, 12924, 0, 1, SYSTEM, 0,   HMIN-FAN-RATIO, 0, STD, 555, 115,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Minimum allowable air flow through heating fan for dual duct systems"
       
          EDIT, 14594, 12930, 0, 1, SYSTEM, 0,    MAX-FAN-RATIO, 0, STD, 650,  65,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Max allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
;2ndrow   EDIT, 14594, 12930, 0, 1, SYSTEM, 0,    MAX-FAN-RATIO, 0, STD, 650,  90,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Max allowable air flow through main fan for single duct (or cooling fan for dual duct systems)"
;         EDIT, 12931, 12931, 0, 1, SYSTEM, 0,   HMAX-FAN-RATIO, 0, STD, 650, 115,  23,  80,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Maximum allowable air flow through heating fan for dual duct systems"
        ENDCASE     
          
; SAC 11/23/10 - removed          
;         LABEL, "Dual Speed Fan/Compressor Ratios", STD, LEFT, 35, 250, 1, 0, 0, 265, 0, 3
;          EDIT, 13118, 13118, 0, 1, SYSTEM, 0, LOW-SPEED-RATIOS, 0, STD,  35, 275,  23,  50,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Ratios of low speed air-flow, energy input, heat and cool capacities to those at high speed"
;          EDIT, 13119, 13119, 0, 1, SYSTEM, 0, LOW-SPEED-RATIOS, 1, STD,  95, 275,  23,  50,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Ratios of low speed air-flow, energy input, heat and cool capacities to those at high speed"
;          EDIT, 13120, 13120, 0, 1, SYSTEM, 0, LOW-SPEED-RATIOS, 2, STD, 155, 275,  23,  50,  2, 3,                        "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Ratios of low speed air-flow, energy input, heat and cool capacities to those at high speed"
;          EDIT, 13121, 13121, 0, 1, SYSTEM, 0, LOW-SPEED-RATIOS, 3, STD, 215, 275,  23,  50,  2, 3,                        "", LEFT,   -2, 5, 1, LEFT, 4, 5, "Ratios of low speed air-flow, energy input, heat and cool capacities to those at high speed"
          
         COMBO, 13116, 13116, 0, 1, SYSTEM, 0,  MIN-FLOW-SOURCE, 0, STD, 490, 200, 115, 120, 19, 3,        "Min Flow Source:", LEFT, -115, 5, 0, LEFT, 4, 5, "Source of makeup air when the supply airflow falls below the Minimum Flow Ratio"
         COMBO, 13115, 12310, 0, 1, SYSTEM, 0,  INDOOR-FAN-MODE, 0, STD, 490, 225,  70, 120, 19, 3,        "Indoor Fan Mode:", LEFT, -115, 5, 0, LEFT, 4, 5, "Controls the operation of indoor fans within the deadband"
          EDIT, 14512, 14512, 0, 1, SYSTEM, 0,  INDUCTION-RATIO, 0, STD, 490, 250,  23,  60,  2, 3,        "Induction Ratio:", LEFT, -115, 5, 1, LEFT, 4, 5, "The ratio of induced air flow to primary air flow"
          EDIT, 12912, 12912, 0, 1, SYSTEM, 0, RETURN-CAP-RATIO, 0, STD, 490, 275,  23,  60,  2, 3,       "Return Cap Ratio:", LEFT, -115, 5, 1, LEFT, 4, 5, "Ratio of the default return (relief) fan capacity to the supply capacity"


       SUBTABPAGE, 3173, 29048, 1, 3, "   Night Cycle Control   "

         LABEL, "Night Venting", STD, LEFT, 25, 55, 1, 0, 0, 320, 12935, 3
         COMBO, 12935, 12935, 0, 1, SYSTEM, 0,  NIGHT-VENT-CTRL, 0, STD, 180,  75, 130, 140, 19, 3,   "Night Vent Control:", LEFT, -140, 5, 0, LEFT, 4, 5, "Behavior of night fans when supply fans are off and Night Cycle Control hasn't cycled fans on"
         COMBO, 12934, 12934, 0, 1, SYSTEM, 0,   NIGHT-VENT-SCH, 0, STD, 180, 100, 200, 140, 19, 3,  "Night Vent Schedule:", LEFT, -140, 5, 0, LEFT, 4, 5, "The hours when night ventilation fans are allowed to run (if the main fans are scheduled off)"
         COMBO, 14595, 13175, 0, 1, SYSTEM, 0,    VENT-TEMP-SCH, 0, STD, 180, 125, 200, 140, 19, 3, "Vent Temperature Sch:", LEFT, -140, 5, 0, LEFT, 4, 5, ""
          EDIT, 12937, 12937, 0, 1, SYSTEM, 0,    NIGHT-VENT-DT, 0, STD, 180, 150,  23,  50,  2, 3,   "Night Vent Delta T:", LEFT, -140, 5, 1, LEFT, 4, 5, "Night Vent Fans only operate if outside drybulb temp is < Control Zone temp by this amount"

         LABEL, "Night Vent Ratios", STD, LEFT, 40, 180, 1, 0, 0, 385, 12936, 3
          EDIT, 12936, 12936, 0, 1, SYSTEM, 0, NIGHT-VENT-RATIO, 0, STD, 180, 200,  23,  50,  2, 3,           "Supply CFM:", LEFT,  -80, 5, 0, LEFT, 4, 5, "Air flow rate, power consumption, and temperature rise in the air due to the night fans"
          EDIT, 14558, 12936, 0, 1, SYSTEM, 0, NIGHT-VENT-RATIO, 1, STD, 180, 225,  23,  50,  2, 3,            "Supply kW:", LEFT,  -80, 5, 0, LEFT, 4, 5, "Air flow rate, power consumption, and temperature rise in the air due to the night fans"
          EDIT, 14559, 12936, 0, 1, SYSTEM, 0, NIGHT-VENT-RATIO, 2, STD, 180, 250,  23,  50,  2, 3,            "Supply dT:", LEFT,  -80, 5, 0, LEFT, 4, 5, "Air flow rate, power consumption, and temperature rise in the air due to the night fans"
          EDIT, 14560, 12936, 0, 1, SYSTEM, 0, NIGHT-VENT-RATIO, 3, STD, 335, 200,  23,  50,  2, 3,           "Return CFM:", LEFT,  -80, 5, 0, LEFT, 4, 5, "Air flow rate, power consumption, and temperature rise in the air due to the night fans"
          EDIT, 14561, 12936, 0, 1, SYSTEM, 0, NIGHT-VENT-RATIO, 4, STD, 335, 225,  23,  50,  2, 3,            "Return kW:", LEFT,  -80, 5, 0, LEFT, 4, 5, "Air flow rate, power consumption, and temperature rise in the air due to the night fans"
          EDIT, 14562, 12936, 0, 1, SYSTEM, 0, NIGHT-VENT-RATIO, 5, STD, 335, 250,  23,  50,  2, 3,            "Return dT:", LEFT,  -80, 5, 0, LEFT, 4, 5, "Air flow rate, power consumption, and temperature rise in the air due to the night fans"

         LABEL, "Night Cycle Fan Control", STD, LEFT, 390, 55, 1, 0, 0, 650, 12932, 3
         COMBO, 12932, 12932, 0, 1, SYSTEM, 0, NIGHT-CYCLE-CTRL, 0, STD, 530,  75, 115, 120, 19, 3,  "Night Cycle Control:", LEFT, -125, 5, 0, LEFT, 4, 5, "The behavior of the system fans when the fan schedule is 'off' (when Fan Schedule value=0)"
         COMBO, 12933, 12933, 0, 1, SYSTEM, 0, NIGHT-CYCLE-FANS, 0, STD, 530, 100,  70, 120, 19, 3,     "Night Cycle Fans:", LEFT, -125, 5, 0, LEFT, 4, 5, "Whether one or both supply fans can operate during Night Cycle Control operation"

    
    ;*****************************************
    ; Outdoor Air 
    ;*****************************************
    TABPAGE, 3054, 10243, 1, 3, NOTIMP, " Outdoor Air "

;  RADIOFIRST, 29025, 29025, 0, 1, 0, PowerDOE, 0, SysModeOA,    0, 0, STD,  23, 14,  18, 185, 3, "Outside Air && Economizer", LEFT, ""
;  RADIONEXT,  29026, 29026, 0, 1, 0, PowerDOE, 0, SysModeOA2,   0, 1, STD, 243, 14,  18, 150, 3,             "Heat Recovery", LEFT, ""
;  RADIONEXT,  29027, 29027, 0, 1, 0, PowerDOE, 0, SysModeOA3,   0, 2, STD, 418, 14,  18, 150, 3,       "Natural Ventilation", LEFT, ""

       SUBTABPAGE, 3174, 29025, 1, 3, "   Outside Air and Economizer   "

         ; SAC 8/26/09 - minor re-positioning
         LABEL, "Outdoor Ventilation Air", STD, LEFT, 30, 30, 1, 0, 0, 400, 12329, 3
          EDIT, 12329, 13088, 0, 1, SYSTEM, 0,  MIN-OUTSIDE-AIR, 0, STD, 220,  50,  23,  50,  2, 3,       "Minimum Outside Air:", LEFT, -175, 5, 1, LEFT, 4, 5, ""
         COMBO, 13234, 13446, 0, 1, SYSTEM, 0,    MIN-OA-METHOD, 0, STD, 220,  75, 200, 180, 19, 3, "Minimum OA Control Method:", LEFT, -175, 5, 0, LEFT, 4, 5, "The method to calculate minimum outside air fraction each hour"
         COMBO, 17955, 13446, 0, 1, SYSTEM, 0, OA-SIZING-METHOD, 0, STD, 220, 100, 200, 180, 19, 3,  "Minimum OA Sizing Method:", LEFT, -175, 5, 0, LEFT, 4, 5, "The method to calculate design minimum outside air fraction each hour"
; SAC 3/2/11 - inserted new DOE-2.3 ZONE-OA-METHOD control (and shifted ALL other controls on this screen down)
         COMBO, 19327, 19327, 0, 1, SYSTEM, 0,   ZONE-OA-METHOD, 0, STD, 220, 125, 200, 180, 19, 3,    "Zone OA Control Method:", LEFT, -175, 5, 0, LEFT, 4, 5, "Whether OA is the maximum of occupant/area requirements, or the sum"
         COMBO, 12909, 13446, 0, 1, SYSTEM, 0,      MIN-AIR-SCH, 0, STD, 220, 150, 200, 180, 19, 3,      "Minimum Air Schedule:", LEFT, -175, 5, 0, LEFT, 4, 5, "The ratio of minimum outside air flow to Supply Air Flow for each hour"
; DEM 10/26/16 - changed to DOAS
;         COMBO, 12910, 12910, 0, 1, SYSTEM, 0,   OA-FROM-SYSTEM, 0, STD, 220, 175, 200, 180, 19, 3,   "Outside Air from System:", LEFT, -175, 5, 0, LEFT, 4, 5, "Name of another system that supplies make-up air to this system"
         COMBO, 19450, 19450, 0, 1, SYSTEM, 0,       DOA-SYSTEM,  0, STD, 600,  50, 300, 150, 19, 3,             "DOA System:",  LEFT, -125, 5, 0, LEFT, 4, 5,"U-name of the dedicated outdoor air system that provides ventilation air to the system."
         COMBO, 19451, 19451, 0, 1, SYSTEM, 0, DOAS-ATTACHED-TO,  0, STD, 600,  75, 300, 150, 19, 3,       "DOAS Attached To:",  LEFT, -125, 5, 0, LEFT, 4, 5,"Specifies whether DOAS provides outdoor air to mixed air section of AHU or directly to the conditioned zones."
         
         LABEL, "Air-Side Economizer Cycle", STD, LEFT, 30, 220, 1, 0, 0, 650, 13160, 3
         COMBO, 13160, 13093, 0, 1, SYSTEM, 0,       OA-CONTROL, 0, STD, 170, 240, 115, 120, 19, 3,       "Outside Air Control:", LEFT, -125, 5, 0, LEFT, 4, 5, ""
          EDIT, 13161, 13448, 0, 1, SYSTEM, 0,    DRYBULB-LIMIT, 0, STD, 170, 265,  23,  50,  1, 3,        "Drybulb High Limit:", LEFT, -125, 5, 1, LEFT, 4, 5, "If outside air temp is above this value economizer dampers close to their minimum setting"
          EDIT, 13162, 13449, 0, 1, SYSTEM, 0,   ENTHALPY-LIMIT, 0, STD, 170, 290,  23,  50,  1, 3,       "Enthalpy High Limit:", LEFT, -125, 5, 1, LEFT, 4, 5, "Outside air enthalpy above which economizer's outside air damper returns to its min position"
      ; SAC 1/9/10 - added more enonomizer controls (requested by Taylor - SDG)
         LABEL, "Return & Outside Air Deltas", STD, LEFT, 45, 320, 1, 0, 0, 260, 0, 3
          EDIT, 19201, 19201, 0, 1, SYSTEM, 0,     DUAL-TEMP-DT, 0, STD, 170, 340,  23,  50,  1, 3,               "Temperature:", LEFT, -110, 5, 1, LEFT, 4, 5, "an optional differential between the return air and the outside air temperatures"
          EDIT, 19202, 19202, 0, 1, SYSTEM, 0, DUAL-ENTHALPY-DH, 0, STD, 170, 365,  23,  50,  1, 3,                  "Enthalpy:", LEFT, -110, 5, 1, LEFT, 4, 5, "an optional differential between the return air and the outside air enthalpies"

         COMBO, 19203, 19203, 0, 1, SYSTEM, 0,   ECONO-SCHEDULE, 0, STD, 500, 240,  85, 150, 19, 3,       "Economizer Schedule:", LEFT, -140, 5, 0, LEFT, 4, 5, "Economizer Schedule - a value of 0 forces the economizer to its minimum position and 1 allows normal economizer operation"
         COMBO, 13163, 13454, 0, 1, SYSTEM, 0,    ECONO-LOCKOUT, 0, STD, 500, 265,  85, 100, 19, 3,        "Lockout Compressor:", LEFT, -140, 5, 0, LEFT, 4, 5, "Whether the compressor is allowed to turn on when the economizer is open"
          EDIT, 13164, 13455, 0, 1, SYSTEM, 0,  ECONO-LOW-LIMIT, 0, STD, 500, 290,  23,  70,  1, 3,      "Economizer Low Limit:", LEFT, -140, 5, 1, LEFT, 4, 5, "Outdoor air (drybulb) temp below which outside dampers are returned to their min position "
          EDIT, 13165, 13456, 0, 1, SYSTEM, 0,  MAX-OA-FRACTION, 0, STD, 500, 315,  23,  70,  2, 3,       "Maximum OA Fraction:", LEFT, -140, 5, 1, LEFT, 4, 5, "Max outside air flow rate when the economizer is operating (as a fraction of the supply air)"
          EDIT, 19204, 19204, 0, 1, SYSTEM, 0,      ECONO-MAX-W, 0, STD, 500, 340,  23,  70,  5, 3,       "Maximum OA Humidity:", LEFT, -140, 5, 1, LEFT, 4, 5, "maximum outdoor-air humidity ratio above which the outside air dampers return to their minimum position"
          EDIT, 19205, 19205, 0, 1, SYSTEM, 0,      ECONO-MIN-W, 0, STD, 500, 365,  23,  70,  5, 3,          "Minimum Humidity:", LEFT, -140, 5, 1, LEFT, 4, 5, "minimum mixed-air humidity ratio below which the outside air dampers return to their minimum position"
; SAC 11/24/10 - added
          EDIT, 19235, 19235, 0, 1, SYSTEM, 0,  ECONO-MIN-DEWPT, 0, STD, 500, 390,  23,  70,  1, 3,          "Minimum Dewpoint:", LEFT, -140, 5, 1, LEFT, 4, 5, "Minimum outdoor-air dewpoint below which the outside air dampers return to their minimum position"

; SAC 10/28/01 - Removed certain keywords
;       SUBTABPAGE, 3175, 29026, 1, 3, "   Heat Recovery   "
;
;          LABEL, "Heat Recovery", STD, LEFT, 30, 30, 1, 0, 0, 380, 13166, 3
;          COMBO, 13166, 13451, 0, 1, SYSTEM, 0,     RECOV-MODE, 0, STD, 230,  50, 100, 150, 19, 3,                  "Recovery Mode:", LEFT, -185, 5, 0, LEFT, 4, 5, "Specifies the mode of heat recovery between central exhaust air and supply air (if any)"
;          COMBO, 13167, 13167, 0, 1, SYSTEM, 0,      RECOV-SCH, 0, STD, 230,  75, 200, 150, 19, 3,              "Recovery Schedule:", LEFT, -185, 5, 0, LEFT, 4, 5, "Specifies the hours of operation of the heat recovery equipment"
;           EDIT, 13168, 13168, 0, 1, SYSTEM, 0,       RECOV-KW, 0, STD, 230, 100,  23,  40,  2, 3,                    "Recovery kW:", LEFT, -185, 5, 1, LEFT, 4, 5, "The power consumed by the recovery equipment whenever it is in operation"
;           
;           EDIT, 13169, 13452, 0, 1, SYSTEM, 0,      RECOV-EFF, 0, STD, 230, 125,  23,  40,  2, 3,  "Design Sensible Effectiveness:", LEFT, -185, 5, 0, LEFT, 4, 5, "Design sensible eff. of heat recovery system (at 10°F delta T and design min outside air)"
; ;         EDIT, 13170, 13453, 0, 1, SYSTEM, 0,    *RECOV-LEFF, 0, STD, 230, 150,  23,  40,  2, 3,    "Design Latent Effectiveness:", LEFT, -185, 5, 0, LEFT, 4, 5, "Design latent eff. of heat recovery system (at 10°F delta T and design min outside air)"
;           
;          LABEL, "Part Load Effectiveness", STD,   LEFT,  30, 214, 1, 0, 0, 445,     0, 3
;          LABEL,                "Sensible", STD, CENTER, 370, 234, 1, 0, 0,   0, 13171, 3
; ;        LABEL,                  "Latent", STD, CENTER, 535, 234, 1, 0, 0,   0, 13172, 3
;          
;          COMBO, 13171, 13171, 0, 1, SYSTEM, 0,   RECOV-EFF-FDT, 0, STD, 295, 250, 200, 150, 19, 3, "f(entering/leaving delta t, % outdoor air):", LEFT, -250, 5, 0, LEFT, 4, 5, "Bi-Quadratic Equation:heat recovery sensible eff. as function of delta t and % outdoor air"
; ;        COMBO, 13172, 13172, 0, 1, SYSTEM, 0, *RECOV-LEFF-FDT, 0, STD, 460, 250, 200, 150, 19, 3,                                            "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Bi-Quadratic Equation:heat recovery latent eff. as function of delta t and % outdoor air"

; SAC 10/6/03 - Implemented new Heat Recovery (ERV) tabs based on designs from MSA
       SUBTABPAGE, 3175, 29026, 1, 3, "   Heat Recovery 1   "

          LABEL, "Basic Specifications", STD, LEFT, 25, 25, 1, 0, 0, 275, 13166, 3
          COMBO, 13166,     0, 0, 1, SYSTEM, 0,  RECOVER-EXHAUST, 0, STD, 185,  45, 100,  90, 19, 3,           "ERV Device Installed:", LEFT, -150, 5, 0, LEFT, 4, 5, "presence of an energy recovery ventilator (heat recovery) between central relief and outside makeup air"
          COMBO, 13167,     0, 0, 1, SYSTEM, 0, ERV-RECOVER-TYPE, 0, STD, 145,  70, 160, 130, 19, 3,                "ERV Device Type:", LEFT, -110, 5, 0, LEFT, 4, 5, "the type of energy recovery ventilator (heat recovery) device between central relief and outside makeup air"

           EDIT, 13168,     0, 0, 1, SYSTEM, 0,      ERV-OA-FLOW, 0, STD, 185,  95,  23,  65,  2, 3,         "Design Outdoor Airflow:", LEFT, -150, 5, 1, LEFT, 4, 5, "the design outdoor airflow at which the ERV is rated"
           EDIT, 13169,     0, 0, 1, SYSTEM, 0,     ERV-EXH-FLOW, 0, STD, 185, 120,  23,  65,  2, 3,         "Design Exhaust Airflow:", LEFT, -150, 5, 1, LEFT, 4, 5, "the design exhaust airflow at which the ERV is rated"
           EDIT, 13170,     0, 0, 1, SYSTEM, 0,        ERV-PURGE, 0, STD, 185, 145,  23,  65,  4, 3,         "OSA Increase for Purge:", LEFT, -150, 5, 1, LEFT, 4, 5, "the fractional increase in the design outdoor airflow that purges the heat wheel"

          LABEL, "HX Performance", STD, LEFT, 330, 25, 1, 0, 0, 650, 13171, 3
          COMBO, 13171,     0, 0, 1, SYSTEM, 0,    ERV-HX-CONFIG, 0, STD, 465,  45, 200, 185, 19, 3,               "HX Configuration:", LEFT, -120, 5, 0, LEFT, 4, 5, "the heat exchanger configuration"
          LABEL, "Sensible", STD, CENTER, 500, 77, 1, 0, 0, 0, 17790, 3
          LABEL, "Latent",   STD, CENTER, 585, 77, 1, 0, 0, 0, 17793, 3
           EDIT, 17790,     0, 0, 1, SYSTEM, 0, ERV-SENSIBLE-EFF, 0, STD, 465,  95,  23,  70,  4, 3,                  "Effectiveness:", LEFT, -120, 5, 0, LEFT, 4, 5, "the sensible effectiveness at the design airflow"
           EDIT, 17791,     0, 0, 1, SYSTEM, 0, ERV-SEN-FILM-RES, 0, STD, 465, 120,  23,  70,  4, 3,             "HX Air Film Resist:", LEFT, -120, 5, 0, LEFT, 4, 5, "the fraction of the design heat-exchanger resistance (1/UA) that is due to the air films"
           EDIT, 17792,     0, 0, 1, SYSTEM, 0, ERV-SEN-FILM-EXP, 0, STD, 465, 145,  23,  70,  4, 3,            "Air Film Resist Exp:", LEFT, -120, 5, 0, LEFT, 4, 5, "the exponent used to vary an air film resistance as a function of the hourly airflow"
           EDIT, 17793,     0, 0, 1, SYSTEM, 0,   ERV-LATENT-EFF, 0, STD, 550,  95,  23,  70,  4, 3,                                "", LEFT,    0, 0, 1, LEFT, 4, 5, "the latent effectiveness at the design airflow"
           EDIT, 17794,     0, 0, 1, SYSTEM, 0, ERV-LAT-FILM-RES, 0, STD, 550, 120,  23,  70,  4, 3,                                "", LEFT,    0, 0, 1, LEFT, 4, 5, "the fraction of the design latent heat exchanger resistance (1/UA) that is due to the air films"
           EDIT, 17795,     0, 0, 1, SYSTEM, 0, ERV-LAT-FILM-EXP, 0, STD, 550, 145,  23,  70,  4, 3,                                "", LEFT,    0, 0, 1, LEFT, 4, 5, "the exponent used to vary an latent air film resistance as a function of the hourly airflow"

          LABEL, "Control Sequences", STD, LEFT, 25, 195, 1, 0, 0, 650, 17810, 3
          COMBO, 17810,     0, 0, 1, SYSTEM, 0,     ERV-RUN-CTRL, 0, STD, 115, 215, 200, 175, 19, 3,                      "Operation:", LEFT,  -80, 5, 0, LEFT, 4, 5, "determines when the ERV will operate"
          COMBO, 17811,     0, 0, 1, SYSTEM, 0,     ERV-SCHEDULE, 0, STD, 115, 240, 200, 175, 19, 3,                       "Schedule:", LEFT,  -80, 5, 0, LEFT, 4, 5, "the schedule that defines when the ERV operates"
           EDIT, 17812,     0, 0, 1, SYSTEM, 0,    OA-EXHAUST-DT, 0, STD, 210, 265,  23,  55,  2, 3,      "Outsd / Exhst Air Delta T:", LEFT, -175, 5, 1, LEFT, 4, 5, "the temperature differential between the outside air and exhaust air streams"
           EDIT, 17813,     0, 0, 1, SYSTEM, 0,    OA-EXHAUST-DH, 0, STD, 210, 290,  23,  55,  2, 3,   "Outsd / Exhst Air Delta Enth:", LEFT, -175, 5, 1, LEFT, 4, 5, "the enthalpy differential between the outside air and exhaust air streams"
          COMBO, 17815,     0, 0, 1, SYSTEM, 0, ERV-RECOVER-MODE, 0, STD, 485, 215, 200, 165, 19, 3,                 "Operating Mode:", LEFT, -140, 5, 0, LEFT, 4, 5, "determines when the ERV will operate"
          COMBO, 17816,     0, 0, 1, SYSTEM, 0,    ERV-TEMP-CTRL, 0, STD, 485, 240, 200, 165, 19, 3,          "Make-up Air Temp Ctrl:", LEFT, -140, 5, 0, LEFT, 4, 5, "the mechanism used to control the make-up air temperature leaving the ERV"
          COMBO, 17817,     0, 0, 1, SYSTEM, 0,     ERV-CAP-CTRL, 0, STD, 485, 265, 200, 165, 19, 3,               "Capacity Control:", LEFT, -140, 5, 0, LEFT, 4, 5, "describes the ERV capacity control mechanism"
           EDIT, 17818,     0, 0, 1, SYSTEM, 0,  OA-HEAT-SETPT-T, 0, STD, 520, 290,  23,  50,  1, 3,    "Make-up Air Heat/Cool Setpt:", LEFT, -175, 5, 0, LEFT, 4, 5, "the outlet make-up air temperature setpoint when the air handler is in the heating mode (return temperature less than required mixed-air temperature)"
           EDIT, 17819,     0, 0, 1, SYSTEM, 0,  OA-COOL-SETPT-T, 0, STD, 585, 290,  23,  50,  1, 3,                                "", LEFT,    0, 0, 1, LEFT, 4, 5, "the outlet make-up air temperature setpoint when the air handler is in the cooling mode (return temperature greater than required mixed-air temperature)"


       SUBTABPAGE, 3359, 29026, 1, 3, "   Heat Recovery 2   "

          LABEL, "ERV Power", STD, LEFT, 25, 15, 1, 0, 0, 650, 17782, 3
           EDIT, 17782,     0, 0, 1, SYSTEM, 0,        ERV-HX-KW, 0, STD, 115,  35,  23,  50,  2, 3,            "HX Power:", LEFT,  -80, 5, 1, LEFT, 4, 5, "the power consumption of the heat-exchanger"
           EDIT, 17783,     0, 0, 1, SYSTEM, 0,   ERV-HX-KW/FLOW, 0, STD, 195,  35,  23,  75,  6, 3,                     "", LEFT,    0, 0, 1, LEFT, 4, 5, "the power consumption of the heat-exchanger per unit of flow"
          COMBO, 17784,     0, 0, 1, SYSTEM, 0,   ERV-HX-KW-FPLR, 0, STD, 130,  60, 200, 165, 19, 3,      "ERV Pwr f(PLR):", LEFT,  -95, 5, 0, LEFT, 4, 5, "a curve that modifies the heat-exchanger power consumption as a function of part load ratio"
          COMBO, 17785,     0, 0, 1, SYSTEM, 0,         ERV-FANS, 0, STD, 130,  85, 200, 165, 19, 3,            "ERV Fans:", LEFT,  -95, 5, 0, LEFT, 4, 5, "whether an ERV uses its own fans to overcome the pressure drop of the heat-exchange media, or the HVAC supply/return fans"
           EDIT, 17786,     0, 0, 1, SYSTEM, 0,      ERV-FAN-EFF, 0, STD, 195, 110,  23,  75,  4, 3,  "ERV Fan Efficiency:", LEFT, -160, 5, 1, LEFT, 4, 5, "the mechanical efficiency of the ERV fans"
          COMBO, 17787,     0, 0, 1, SYSTEM, 0,  ERV-MOTOR-CLASS, 0, STD, 130, 135, 200, 165, 19, 3,       "Fan Motor Eff:", LEFT,  -95, 5, 0, LEFT, 4, 5, "the motor class (efficiency) of the ERV fans"
          COMBO, 17788,     0, 0, 1, SYSTEM, 0, ERV-FAN-KW-FFLOW, 0, STD, 130, 160, 200, 165, 19, 3,     "Fan Pwr f(flow):", LEFT,  -95, 5, 0, LEFT, 4, 5, "a curve that modifies the hourly fan power consumption as a function of airflow"

          LABEL, "Make-Up",  STD, CENTER, 501, 42, 1, 0, 0, 0, 17782, 3
          LABEL, "Exhaust",  STD, CENTER, 579, 42, 1, 0, 0, 0, 17782, 3
           EDIT, 17800,     0, 0, 1, SYSTEM, 0,        ERV-OA-KW, 0, STD, 469,  60,  23,  63,  4, 3,          "Fan Pwr @ Dsgn Flow:", LEFT, -129, 5, 0, LEFT, 4, 5, "the power consumption of the outside air makeup fan at the design outdoor airflow at which the ERV is rated"
           EDIT, 17801,     0, 0, 1, SYSTEM, 0,   ERV-OA-KW/FLOW, 0, STD, 469,  85,  23,  63,  4, 3,          "Fan Pwr / Unit Flow:", LEFT, -129, 5, 0, LEFT, 4, 5, "the power consumption of the outside air makeup fan, normalized to the design outdoor airflow at which the ERV is rated"
           EDIT, 17802,     0, 0, 1, SYSTEM, 0,    ERV-OA-STATIC, 0, STD, 469, 110,  23,  63,  4, 3,          "Delta P @ Dsgn Flow:", LEFT, -129, 5, 0, LEFT, 4, 5, "the static pressure drop of the air flowing through the outside-air side of the heat-exchanger at the design outdoor airflow at which the ERV is rated"
           EDIT, 17804,     0, 0, 1, SYSTEM, 0,       ERV-EXH-KW, 0, STD, 547,  60,  23,  63,  4, 3,                              "", LEFT,    0, 0, 1, LEFT, 4, 5, "the power consumption of the outside air makeup fan at the design exhaust airflow at which the ERV is rated"
           EDIT, 17805,     0, 0, 1, SYSTEM, 0,  ERV-EXH-KW/FLOW, 0, STD, 547,  85,  23,  63,  4, 3,                              "", LEFT,    0, 0, 1, LEFT, 4, 5, "the power consumption of the outside air makeup fan, normalized to the design exhaust airflow at which the ERV is rated"
           EDIT, 17806,     0, 0, 1, SYSTEM, 0,   ERV-EXH-STATIC, 0, STD, 547, 110,  23,  63,  4, 3,                              "", LEFT,    0, 0, 1, LEFT, 4, 5, "the static pressure drop of the air flowing through the outside-air side of the heat-exchanger at the design exhaust airflow at which the ERV is rated"
           EDIT, 17807,     0, 0, 1, SYSTEM, 0,   ERV-STATIC-EXP, 0, STD, 547, 135,  23,  63,  4, 3,       "Pressure Drop Exponent:", LEFT, -207, 5, 1, LEFT, 4, 5, "an exponent that modifies the outside or exhaust static pressure drop as a function of airflow"

          LABEL, "Condensation/Frost Control", STD, LEFT, 25, 200, 1, 0, 0, 650, 17820, 3
          COMBO, 17820,     0, 0, 1, SYSTEM, 0,   ERV-FROST-CTRL, 0, STD, 145, 220, 200, 150, 19, 3,              "Cond/Frost Ctrl:", LEFT, -110, 5, 0, LEFT, 4, 5, "the condensate/frost control methodology"
          COMBO, 17821,     0, 0, 1, SYSTEM, 0, ERV-PREHEAT-CTRL, 0, STD, 145, 245, 200, 150, 19, 3,             "ERV Preheat Ctrl:", LEFT, -110, 5, 0, LEFT, 4, 5, "the preheat temperature control strategy"
;          COMBO, 17822,     0, 0, 1, SYSTEM, 0,  ERV-PREHEAT-SRC, 0, STD, 145, 270, 200, 150, 19, 3,               "Preheat Source:", LEFT, -110, 5, 0, LEFT, 4, 5, "the type of preheat coil"
;           EDIT, 17824,     0, 0, 1, SYSTEM, 0,    ERV-PREHEAT-T, 0, STD, 545, 220,  23,  55,  1, 3,      "Preheat Setpoint Temperature:", LEFT, -205, 5, 1, LEFT, 4, 5, "the preheat setpoint temperature"
;           EDIT, 17824,     0, 0, 1, SYSTEM, 0,   PREHEAT-AIR-DT, 0, STD, 545, 245,  23,  55,  2, 3,               "Preheat Air Delta T:", LEFT, -205, 5, 1, LEFT, 4, 5, "the design air temperature rise through the preheat coil"
;           EDIT, 17824,     0, 0, 1, SYSTEM, 0,    PREHEAT-HW-DT, 0, STD, 545, 270,  23,  55,  2, 3,             "Preheat Water Delta T:", LEFT, -205, 5, 1, LEFT, 4, 5, "the design water temperature drop through the preheat coil"
;           EDIT, 17824,     0, 0, 1, SYSTEM, 0, PREHEAT-INLET-DT, 0, STD, 545, 295,  23,  55,  2, 3, "Preheat Inlet Water & Air Delta T:", LEFT, -205, 5, 1, LEFT, 4, 5, "the design temperature differential between the hot-water entering the preheat coil and the air entering the preheat coil"


       SUBTABPAGE, 3176, 29027, 1, 3, "   Natural Ventilation   "

         LABEL, "Natural Ventilation", STD, LEFT, 30, 30, 1, 0, 0, 420, 13173, 3
         COMBO, 13173, 13450, 0, 1, SYSTEM, 0,      VENT-METHOD, 0, STD, 240,  50, 150, 180, 19, 3,            "Ventilation Method:", LEFT, -195, 5, 0, LEFT, 4, 5, "When windows open: Air Change=Constant vent ;S-G=Ventilation is function of wind speed"
         COMBO, 13174, 13174, 0, 1, SYSTEM, 0, NATURAL-VENT-SCH, 0, STD, 240,  75, 200, 180, 19, 3,             "Vent Use Schedule:", LEFT, -195, 5, 0, LEFT, 4, 5, "Specifies when the windows can be open and when they are always closed"
         COMBO, 13175, 13175, 0, 1, SYSTEM, 0,    VENT-TEMP-SCH, 0, STD, 240, 100, 200, 180, 19, 3, "Ventilation Temperature Sched:", LEFT, -195, 5, 0, LEFT, 4, 5, "Hourly indoor drybulb temperatures that natural ventilation attempts to achieve"
         COMBO, 13176, 13176, 0, 1, SYSTEM, 0,    OPEN-VENT-SCH, 0, STD, 240, 125, 200, 180, 19, 3, "Window Open Probability Sched:", LEFT, -195, 5, 0, LEFT, 4, 5, "Probability that windows will be opened if conditions warrant natural ventilation"
         
         LABEL, "Sherman-Grimsrud Method", STD, LEFT, 30, 190, 1, 0, 0, 320, 13177, 3
          EDIT, 13177, 13177, 0, 1, SYSTEM, 0,    MAX-VENT-RATE, 0, STD, 230, 210,  23,  50,  1, 3,      "Air Changes / Hour (max):", LEFT, -185, 5, 1, LEFT, 4, 5, "Maximum number of air changes per hour due to natural ventilation"
          EDIT, 13178, 13178, 0, 1, SYSTEM, 0,   FRAC-VENT-AREA, 0, STD, 230, 235,  23,  50,  2, 3,      "Total Vent Area Fraction:", LEFT, -185, 5, 1, LEFT, 4, 5, "Total leakage area (as a fraction of floor area); typically = 0.6(open window area)/(floor area)"
          EDIT, 13179, 13179, 0, 1, SYSTEM, 0,    HOR-VENT-FRAC, 0, STD, 230, 260,  23,  50,  2, 3, "Horizontal Vent Area Fraction:", LEFT, -185, 5, 1, LEFT, 4, 5, "Fraction of the ventilation area that is in the floor and ceiling"
         
         LABEL, "Air Change Method", STD, LEFT, 345, 190, 1, 0, 0, 620, 13180, 3
          EDIT, 13180, 13180, 0, 1, SYSTEM,  0, NATURAL-VENT-AC, 0, STD, 535, 210,  23,  50,  1, 3,    "Air Changes / Hour (fixed):", LEFT, -165, 5, 1, LEFT, 4, 5, "Number of air changes per hour when the windows are open"

; DEM 02/22/16 - new keywords
         LABEL, "Fan Assisted Natural Ventilation", STD, LEFT, 645, 190, 1, 0, 0, 920, 19340, 3
          EDIT, 19340, 19340, 0, 1, SYSTEM,  0,     FAN-VENT-AC, 0, STD, 845, 210,  23,  50,  1, 3,    "Fan Air Changes / Hour:", LEFT, -165, 5, 1, LEFT, 4, 5, "Number of air changes per hour when fan assist is on"
          EDIT, 19341, 19341, 0, 1, SYSTEM,  0, NATURAL-VENT-KW, 0, STD, 845, 235,  23,  50,  1, 3,    "Nat Vent Fan Power, kW:", LEFT, -165, 5, 1, LEFT, 4, 5, "Power draw for natural ventilation fan at full speed"
          EDIT, 19347, 19347, 0, 1, SYSTEM,  0,      VENT-MAX-T, 0, STD, 845, 260,  23,  50,  1, 3,    "  Max nat vent zone T:", LEFT, -165, 5, 1, LEFT, 4, 5, "Maximum zone temeperature during natural ventilation"

   
    ;*****************************************
    ; Cooling 
    ;*****************************************
    TABPAGE, 3055, 29072, 1, 3, NOTIMP, "  Cooling  "

;  RADIOFIRST, 29028, 29028, 0, 1, 0, PowerDOE, 0, SysModeCooling,    0, 0, STD,  17, 14,  18,  95, 3, "Coil Cap/Ctrl", LEFT, ""
;  RADIONEXT,  29029, 29029, 0, 1, 0, PowerDOE, 0, SysModeCooling2,   0, 1, STD, 120, 14,  18, 100, 3, "Unitary Power", LEFT, ""
;  RADIONEXT,  29030, 29030, 0, 1, 0, PowerDOE, 0, SysModeCooling3,   0, 2, STD, 229, 14,  18,  82, 3,     "Condenser", LEFT, ""
;  RADIONEXT,  29031, 29031, 0, 1, 0, PowerDOE, 0, SysModeCooling4,   0, 3, STD, 320, 14,  18,  85, 3,    "Cap Curves", LEFT, ""
;  RADIONEXT,  29032, 29032, 0, 1, 0, PowerDOE, 0, SysModeCooling5,   0, 4, STD, 414, 14,  18,  97, 3,  "Evap Cooling", LEFT, ""
;  RADIONEXT,  29017, 29017, 0, 1, 0, PowerDOE, 0, SysModeCooling6,   0, 5, STD, 519, 14,  18,  68, 3,         "Econo", LEFT, ""

       SUBTABPAGE, 3177, 29028, 1, 3, "  Coil Capacity / Control  "
; AFR 4/29/09 - increase shadow line length
         LABEL, "Cooling Capacity", STD, LEFT, 15,  5, 1, 0, 0, 430, 13223, 3
; SDG 11/28/06 - Added new keyword COOL-SOURCE
         COMBO, 18313,     0, 0, 1, SYSTEM, 0,      COOL-SOURCE, 0, STD, 155,  25, 190, 150, 19, 3,                   "Cool Source:", LEFT, -125, 5, 0, LEFT, 4, 5, "The source of cooling for the main cooling coil (in the central air distribution system)"

; AFR 4/29/09 - added column labels         
;          LABEL, "", BOLD, LEFT, 360, 25, 1, 0, 0, 615, 0, 1
          LABEL, "GROSS",                      STD, LEFT, 215, 58, 1, 0, 0, 348, 0, 1
          LABEL, "NET",                        STD, LEFT, 350, 58, 1, 0, 0, 430, 0, 1
; AFR 4/29/09 - dropped each line on the left side by 25
          EDIT, 13223, 12285, 0, 1, SYSTEM, 0, COOLING-CAPACITY, 0, STD, 195,  75,  23,  80,  0, 3,        "Total Cooling Capacity:", LEFT, -165, 5, 1, LEFT, 4, 5, "Total cooling capacity (at ARI conditions) of the system's chilled water or DX cooling coil"
          EDIT, 13224, 12286, 0, 1, SYSTEM, 0,      COOL-SH-CAP, 0, STD, 195, 100,  23,  80,  0, 3,     "Sensible Cooling Capacity:", LEFT, -165, 5, 1, LEFT, 4, 5, "Sensible heat removal capacity of the system's air cooling device at ARI rated conditions"
; AFR 4/29/09 - Moved from Compliance /Cooling tab
          EDIT, 15559, 15559, 0, 1, SYSTEM, 0,  C-TOTAL-CLG-CAP, 0, STD, 320,  75,  23,  80,  1, 7,        "", LEFT, -145, 5, 1, LEFT, 4, 5, "The total cooling capacity of all identical units"
; SAC 11/23/10 - added
          EDIT, 19213, 19213, 0, 1, SYSTEM, 0,  SENS-HEAT-RATIO, 0, STD, 230, 125,  23,  45,  2, 3,           "Sensible Heat Ratio:", LEFT, -200, 5, 1, LEFT, 4, 5, "Defines the ratio of sensible to total cooling capacity"
         LABEL, "Rated Entering Temps:", STD, LEFT, 30, 170, 1, 0, 0, 0, 19214, 3
          EDIT, 19214, 19214, 0, 1, SYSTEM, 0,        RATED-EDB, 0, STD, 175, 165,  23,  45,  1, 3,                          "DBT", CENTER, 22, -15, 0, LEFT, 4, 5, "The indoor entering drybulb corresponding to the cooling capacity"
          EDIT, 19215, 19215, 0, 1, SYSTEM, 0,        RATED-EWB, 0, STD, 230, 165,  23,  45,  1, 3,                          "WBT", CENTER, 22, -15, 0, LEFT, 4, 5, "The indoor entering wetbulb corresponding to the cooling capacity"
          EDIT, 19216, 19216, 0, 1, SYSTEM, 0,        RATED-ECT, 0, STD, 285, 165,  23,  45,  1, 3,                        "Cond.", CENTER, 22, -15, 1, LEFT, 4, 5, "The entering condenser temperature corresponding to the cooling capacity"
          
          EDIT, 13222, 13466, 0, 1, SYSTEM, 0, COOL-SIZING-RATI, 0, STD, 230, 190,  23,  45,  2, 3,             "Cool Sizing Ratio:", LEFT, -200, 5, 1, LEFT, 4, 5, "Used to deliberately oversize or undersize the cooling coil capacity"
          EDIT, 13226, 13226, 0, 1, SYSTEM, 0,  COOL-RPM-LIMITS, 0, STD, 170, 215,  23,  55,  0, 3,         "RPM Limits, Max & Min:", LEFT, -140, 5, 0, LEFT, 4, 5, "Maximum engine RPM during cooling (for natural-gas-fired engine-driven heat pumps)"
          EDIT, 13225, 13225, 0, 1, SYSTEM, 0,  COOL-RPM-LIMITS, 1, STD, 230, 215,  23,  45,  0, 3,                               "", LEFT, -220, 5, 1, LEFT, 4, 5, "Minimum engine RPM during cooling (for natural-gas-fired engine-driven heat pumps)"
                                                                                                                               
          EDIT, 13227, 13227, 0, 1, SYSTEM, 0,   COOL-CLOSS-MIN, 0, STD, 230, 240,  23,  45,  2, 3,   "Min Cycling Part Load Ratio:", LEFT, -200, 5, 1, LEFT, 4, 5, "Min cycling PLR for which the Total Cooling Capacity f(PLR) operating curve is valid"
          EDIT, 13228, 13228, 0, 1, SYSTEM, 0,    CHW-COIL-HEAD, 0, STD, 230, 265,  23,  45,  1, 3,                 "CHW Coil Head:", LEFT, -200, 5, 1, LEFT, 4, 5, "Pressure drop through the chilled water coil of the loop fluid (at the design flow rate)"
          EDIT, 13229, 13229, 0, 1, SYSTEM, 0,      CHW-COIL-DT, 0, STD, 230, 290,  23,  45,  1, 3,              "CHW Coil Delta T:", LEFT, -200, 5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flowrate)"
         COMBO, 13246, 13246, 0, 1, SYSTEM, 0,   CHW-VALVE-TYPE, 0, STD, 155, 315,  85, 150, 19, 3,                "CHW Valve Type:", LEFT, -125, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
         COMBO, 19094, 13247, 0, 1, SYSTEM, 0,         CHW-LOOP, 0, STD, 155, 340, 200, 150, 19, 3,                      "CHW Loop:", LEFT, -125, 5, 0, LEFT, 4, 5, "Name of the loop that this system's chilled water coil is attached to"
          EDIT, 13248, 13472, 0, 1, SYSTEM, 0,          COIL-BF, 0, STD, 230, 365,  23,  45,  3, 3,     "Coil Design Bypass Factor:", LEFT, -200, 5, 1, LEFT, 4, 5, "Cooling coil full load bypass factor (at the ARI rating conditions)"
;         EDIT, 13249, 13249, 0, 1, SYSTEM, 0,      COOL-FT-MIN, 0, STD, 230, 390,  23,  45,  1, 3, "Min Bypass Extrapolation Temp:", LEFT, -200, 5, 1, LEFT, 4, 5, "Minimum outside air dry bulb temp for which the cooling Curve Fits are valid"

; AFR 4/29/09 - moved right side control further right by 75 to make room.
; AFR 4/29/09 - increase shadow line length
         LABEL, "Cooling Control and Reset", STD, LEFT, 450,  5, 1, 0, 0, 720, 0, 3
          EDIT, 13211, 12278, 0, 1, SYSTEM, 0,     MIN-SUPPLY-T, 0, STD, 660,  25,  23,  45,  1, 3, "Zone Entering Min Supply Temp:", LEFT, -195, 5, 1, LEFT, 4, 5, ""
          EDIT, 13212, 13470, 0, 1, SYSTEM, 0,       COOL-SET-T, 0, STD, 660,  50,  23,  45,  1, 3,    "Cold Deck Min Leaving Temp:", LEFT, -195, 5, 1, LEFT, 4, 5, "The (constant) cooling supply air temperature; used when Cooling Control = Constant"
          EDIT, 13213, 13213, 0, 1, SYSTEM, 0,  COOL-CTRL-RANGE, 0, STD, 660,  75,  23,  45,  1, 3,            "Cool Control Range:", LEFT, -195, 5, 1, LEFT, 4, 5, "The throttling range of the cooling coil controller"
; 3/27/97 - removed per JJH request
;         EDIT, 13214, 13471, 0, 1, SYSTEM, 0,     MAX-HUMIDITY, 0, STD, 585, ???,  23,  45,  1, 3,              "Maximum Humidity:", LEFT, -195, 5, 1, LEFT, 4, 5, "Highest allowable relative humidity in the return air (from all zones served by the system)"
         COMBO, 13215, 13215, 0, 1, SYSTEM, 0,   MIN-SUPPLY-SCH, 0, STD, 575, 100, 200, 150, 19, 3,                "Min Supply Sch:", LEFT, -110, 5, 0, LEFT, 4, 5, "Lowest allowable temperature for air entering the zones (diffuser air temperature)"
         COMBO, 13216, 13216, 0, 1, SYSTEM, 0,     COOL-SET-SCH, 0, STD, 575, 125, 200, 150, 19, 3,                 "Cold Deck Sch:", LEFT, -110, 5, 0, LEFT, 4, 5, "The temperature of cooling air supply temperature; used when Cooling Control = Scheduled"
         COMBO, 13217, 13473, 0, 1, SYSTEM, 0, COOLING-SCHEDULE, 0, STD, 575, 150, 200, 150, 19, 3,              "Availability Sch:", LEFT, -110, 5, 0, LEFT, 4, 5, "Whether mechanical cooling is allowed (not incl. natural ventilation or Night Cycle Control)"
         COMBO, 13218, 13474, 0, 1, SYSTEM, 0,     COOL-CONTROL, 0, STD, 575, 175, 120, 150, 19, 3,                  "Cool Control:", LEFT, -110, 5, 0, LEFT, 4, 5, "Strategy used to control supply air temperature leaving the systems central cooling coil"
         COMBO, 13219, 13219, 0, 1, SYSTEM, 0,   RESET-PRIORITY, 0, STD, 575, 200, 100, 150, 19, 3,                "Reset Priority:", LEFT, -110, 5, 0, LEFT, 4, 5, "Priority by which supply-air temperature is reset (for Cool Ctrl=warmest or Heat Ctrl=coldest)"
         COMBO, 13220, 13220, 0, 1, SYSTEM, 0,   COOL-RESET-SCH, 0, STD, 575, 225, 200, 150, 19, 3,                "Cool Reset Sch:", LEFT, -110, 5, 0, LEFT, 4, 5, "A Reset Temp Schedule that defines the cooling supply air temp as a fct of outside air temp"
          EDIT, 13221, 13221, 0, 1, SYSTEM, 0, COOL-MAX-RESET-T, 0, STD, 660, 250,  23,  45,  1, 3,    "Maximum Cooling Reset Temp:", LEFT, -195, 5, 1, LEFT, 4, 5, "Maximum temperature that the supply air can be reset to (during cooling)"
          EDIT, 17891, 13221, 0, 1, SYSTEM, 0, COOL-MIN-RESET-T, 0, STD, 660, 275,  23,  45,  1, 3,    "Minimum Cooling Reset Temp:", LEFT, -195, 5, 1, LEFT, 4, 5, "Maximum temperature that the supply air can be reset to (during cooling)"
          EDIT, 17892, 13221, 0, 1, SYSTEM, 0,   MIN-RESET-FLOW, 0, STD, 660, 300,  23,  45,  3, 3,            "Minimum Reset Flow:", LEFT, -195, 5, 1, LEFT, 4, 5, "Maximum flow fraction used for the WARMEST supply air temperature reset (during cooling)"


       SUBTABPAGE, 3178, 29029, 1, 3, "  Unitary Power  "

         LABEL, "Cooling Power", BOLD, LEFT, 20, 25, 1, 0, 0, 310, 0, 3
          EDIT, 13270, 12383, 0, 1, SYSTEM, 0,      COOLING-EIR, 0, STD, 205,  45,  23,  60,  4, 3,  "Cooling Electric Input Ratio:", LEFT, -170,  5, 1, LEFT, 4, 5, ""
; SAC 11/23/10 - added          
         COMBO, 19207, 19207, 0, 1, SYSTEM, 0,      COIL-CONFIG, 0, STD, 175,  70, 200, 135, 19, 3,         "DX Coil Configuration:", LEFT, -140,  5, 0, LEFT, 4, 5, "For multi-compressor units, specifies the configuration of the coil circuits"


      ; SAC 4/23/09 - Moved to here from Compliance / Cooling tab
         LABEL, "Compliance Efficiency Ratings", BOLD, LEFT, 360, 25, 1, 0, 0, 615, 0, 7
         LABEL, "FULL LOAD",                      STD, LEFT, 625, 25, 1, 0, 0, 825, 0, 7
         LABEL, "PART LOAD",                      STD, LEFT, 835, 25, 1, 0, 0, 940, 0, 7

         LABEL, "Seasonal (if applicable):",      STD, LEFT, 375,  50, 1, 0, 0, 0, 15562, 7
         LABEL, "Air/Evaporatively Cooled DX:",   STD, LEFT, 375,  75, 1, 0, 0, 0, 15560, 7
         LABEL, "Water Cooled DX:",               STD, LEFT, 375, 100, 1, 0, 0, 0, 15567, 7
         LABEL, "Ground Water Cooled DX:",        STD, LEFT, 375, 125, 1, 0, 0, 0, 15569, 7

          EDIT, 15562, 15562, 0, 1, SYSTEM, 0,           C-SEER, 0, STD, 615,  45,  23,  80,  2, 7,         "SEER:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The SEER of the air conditioner"
          EDIT, 15561, 15561, 0, 1, SYSTEM, 0,           C-IPLV, 0, STD, 825,  45,  23,  80,  2, 7,         "IPLV:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The IPLV of the air conditioner"
          EDIT, 15560, 15560, 0, 1, SYSTEM, 0,          C-EER95, 0, STD, 615,  70,  23,  80,  2, 7,       "EER 95:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 95F (ODB) of the air cooled air conditioner"
          EDIT, 15566, 15566, 0, 1, SYSTEM, 0,          C-EER82, 0, STD, 825,  70,  23,  80,  2, 7,       "EER 82:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 82F (ODB) of the air cooled air conditioner"
          EDIT, 15567, 15567, 0, 1, SYSTEM, 0,       C-EER85EWT, 0, STD, 615,  95,  23,  80,  2, 7,       "EER 85:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 85F (EWT) of the water source heat pump"
          EDIT, 15568, 15568, 0, 1, SYSTEM, 0,       C-EER75EWT, 0, STD, 825,  95,  23,  80,  2, 7,       "EER 75:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 75F (EWT) of the water source heat pump"
          EDIT, 15569, 15569, 0, 1, SYSTEM, 0,       C-EER70EWT, 0, STD, 615, 120,  23,  80,  2, 7,       "EER 70:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 70F (EWT) of the ground source heat pump"
          EDIT, 15570, 15570, 0, 1, SYSTEM, 0,       C-EER50EWT, 0, STD, 825, 120,  23,  80,  2, 7,       "EER 50:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 50F (EWT) of the ground source heat pump"


         LABEL, "Cooling Compressor", BOLD, LEFT, 20, 215, 1, 0, 0, 300, 0, 3
         COMBO, 13271, 12385, 0, 1, SYSTEM, 0,  COMPRESSOR-TYPE, 0, STD, 165, 235, 100, 120, 19, 3,               "Compressor Type:", LEFT, -130,  5, 0, LEFT, 4, 5, ""
          EDIT, 13272, 13272, 0, 1, SYSTEM, 0, MIN-UNLOAD-RATIO, 0, STD, 210, 260,  23,  60,  2, 3,          "Minimum Unload Ratio:", LEFT, -175,  5, 1, LEFT, 4, 5, "PLR at which compressor unloading stops and hot gas bypass or cycling begins"
          EDIT, 13273, 13273, 0, 1, SYSTEM, 0,    MIN-HGB-RATIO, 0, STD, 210, 285,  23,  60,  2, 3,      "Min Hot Gas Bypass Ratio:", LEFT, -175,  5, 1, LEFT, 4, 5, "The part load ratio below which compressor cycling begins"

         LABEL, "Crankcase Power", BOLD, LEFT, 20, 340, 1, 0, 0, 300, 0, 3
          EDIT, 13274, 13274, 0, 1, SYSTEM, 0,   CRANKCASE-HEAT, 0, STD, 210, 360,  23,  60,  3, 3,                "Crankcase Heat:", LEFT, -175,  5, 1, LEFT, 4, 5, "Electricity consumed to heat the crankcase of direct expansion (DX) compressors"
; DEM 11/28/16 - new keyword
          EDIT, 19479, 19479, 0, 1, SYSTEM, 0,    CRANKCASE-EIR, 0, STD, 210, 385,  23,  60,  3, 3,                 "Crankcase EIR:", LEFT, -175,  5, 1, LEFT, 4, 5, "Normalized electricity to heat the DX crankcase per unit of rated cooling capacity"
          EDIT, 13275, 13275, 0, 1, SYSTEM, 0,  CRANKCASE-MAX-T, 0, STD, 210, 410,  23,  60,  1, 3,     "Crankcase Max Temperature:", LEFT, -175,  5, 1, LEFT, 4, 5, "Outdoor air (drybulb) temp above which the crankcase heater is not allowed to operate"
;SAC 1/15/00   LABEL, "Temperature:", STD, LEFT, 18, 299, 1, 0, 0, 0, 0, 3
 
; SAC 4/23/09 - merged two performance curve sections into one         
;         LABEL, "Cooling Electric Input Ratio Curves", STD, LEFT, 350, 125, 1, 0, 0, 650, 0, 3
         LABEL, "Performance Curves", BOLD, LEFT, 360, 175, 1, 0, 0, 940, 0, 3
         LABEL, "Electric Input Ratio", STD, CENTER, 610, 191, 1, 0, 0, 0, 0, 3
         COMBO, 13276, 13276, 0, 1, SYSTEM, 0,      COOL-EIR-FT, 0, STD, 505, 210, 200, 210, 19, 3,          "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Quadratic Curve Fit: Electric Input Ratio as a function of temp of entering & leaving water"
         LABEL, "t enter condenser):", STD, LEFT,                        387, 222, 1, 0, 0, 0, 13276, 3
;@@      COMBO, 13277, 13277, 0, 1, SYSTEM, 0,      COOL-EIR-FT, 0, STD, 495,  ??, 200, 210, 19, 3,          "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Quadratic Curve Fit: Electric Input Ratio as a function of temp of entering & leaving water"
;@@      LABEL, "t entering water):", STD, LEFT, 377,  72, 1, 0, 0, 0, 13277, 3
;        COMBO, 13278, 13278, 0, 1, SYSTEM, 0, RATED-CEIR-FFLOW, 0, STD, 495,  ??, 200, 210, 19, 3,          "f(supply/rated flow):", LEFT, -130,  5, 0, LEFT, 4, 5, ""
         COMBO, 13279, 13279, 0, 1, SYSTEM, 0,    COOL-EIR-FPLR, 0, STD, 505, 235, 200, 210, 19, 3,            "f(part load ratio):", RIGHT, -10,  5, 0, LEFT, 4, 5, "Cubic Curve Fit: Electric Input Ratio as a function of the part load ratio"
         COMBO, 13280, 13280, 0, 1, SYSTEM, 0,    COOL-EIR-FRPM, 0, STD, 505, 260, 200, 210, 19, 3,                        "f(RPM):", RIGHT, -10,  5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Electric Input Ratio as a function of compressor rpm"

;         LABEL, "Low Speed Electric Input Ratio Curve", STD, LEFT, 350, 250, 1, 0, 0, 650, 13281, 3
         LABEL, "Low Speed Electric Input Ratio", STD, CENTER, 835, 191, 1, 0, 0, 0, 13281, 3
         COMBO, 13281, 13281, 0, 1, SYSTEM, 0,   COOL-EIR-LS-FT, 0, STD, 730, 285, 200, 210, 19, 3,          "f(t entering wetbulb,", LEFT, -355, -4, 0, LEFT, 4, 5, "B-Quadratic Curve Fit: EIR as a function of entering wetbulb temp & outside drybulb temp"
         LABEL, "t outdoor drybulb):", STD, LEFT,                        387, 297, 1, 0, 0, 0, 13281, 3

         LABEL, "Gas Heat Pump Auxiliary Electric", BOLD, LEFT, 360, 340, 1, 0, 0, 605, 14513, 3
          EDIT, 14513, 14513, 0, 1, SYSTEM, 0,   UNIT-PUMP-ELEC, 0, STD, 505, 360,  23,  60,  3, 3,                "Gas HP Pump kW:", LEFT, -130,  5, 1, LEFT, 4, 5, "Pump power for the Gas Heat Pump, or supplemental boiler (per Btu Cooling Capacity)"
          EDIT, 14514, 14514, 0, 1, SYSTEM, 0,      UNIT-AUX-KW, 0, STD, 505, 385,  23,  60,  3, 3,                 "Gas HP Aux kW:", LEFT, -130,  5, 1, LEFT, 4, 5, "Power consumption of Gas Heat Pump's auxiliaries (e.g., controls), that operate continuously"


       SUBTABPAGE, 3179, 29030, 1, 3, "  Condenser  "

         LABEL, "Air-Cooled Condenser & Outdoor Fan", STD, LEFT, 20, 35, 1, 0, 0, 305, 0, 3
         COMBO, 13250, 12386, 0, 1, SYSTEM, 0,   CONDENSER-TYPE, 0, STD, 160,  55, 100, 145, 19, 3,                "Condenser Type:", LEFT, -125,  5, 0, LEFT, 4, 5, "Air Cooled=heat exchanger & condenser; Water Cooled=heat rejection & condenser loop"
         COMBO, 13251, 13476, 0, 1, SYSTEM, 0, OUTSIDE-FAN-MODE, 0, STD, 160,  80,  85, 145, 19, 3,              "Outside Fan Mode:", LEFT, -125,  5, 0, LEFT, 4, 5, "Whether the outside fan cycles with the load or remains on"
          EDIT, 13252, 13252, 0, 1, SYSTEM, 0,    OUTSIDE-FAN-T, 0, STD, 220, 105,  23,  50,  1, 3,       "Outside Fan Temperature:", LEFT, -185,  5, 1, LEFT, 4, 5, "Outside air (drybulb) temp below which the condenser fan is not permitted to operate"
          EDIT, 13253, 13253, 0, 1, SYSTEM, 0, OUTSIDE-FAN-ELEC, 0, STD, 220, 130,  23,  50,  2, 3,          "Outside Fan Electric:", LEFT, -185,  5, 1, LEFT, 4, 5, "power consumption of outside fan (condenser fan when cooling; evaporator fan when heating)"
         COMBO, 13255, 13255, 0, 1, SYSTEM, 0, OUTSIDE-FAN-CFLT, 0, STD, 160, 180, 200, 145, 19, 3,              "Outdoor Fan Pwr =", LEFT, -125, -4, 0, LEFT, 4, 5, "Bi-Quadratic:power consumption of outdoor fan as fct of cooling PLR and cond. entering temp"
         LABEL, "f(cool PLR, osa db):", STD, LEFT, 37, 192, 1, 0, 0, 0, 13255, 3
         COMBO, 13243, 13243, 0, 1, SYSTEM, 0, OUTSIDE-FAN-HFLT, 0, STD, 160, 215, 200, 145, 19, 3,              "Outdoor Fan Pwr =", LEFT, -125, -4, 0, LEFT, 4, 5, "Bi-Quadratic:power consumption of outdoor fan as fct of heating PLR and OA drybulb temp"
         LABEL,    "f(heat PLR, osa db):", STD, LEFT, 37, 227, 1, 0, 0, 0, 13243, 3
          
         LABEL, "Evaporative Precooler",  STD, LEFT, 360,  35, 1, 0, 0, 655, 13260, 3
          EDIT, 13260, 13260, 0, 1, SYSTEM, 0,     EVAP-PCC-EFF, 0, STD, 565,  55,  23,  50,  2, 3,  "Evap Condenser Effectiveness:", LEFT, -190,  5, 1, LEFT, 4, 5, "The effectiveness of the evaporative pre-cooling unit"
         COMBO, 13261, 13261, 0, 1, SYSTEM, 0,     EVAP-PCC-SCH, 0, STD, 500,  80, 200, 150, 19, 3,               "Evap Cond Sched:", LEFT, -125,  5, 0, LEFT, 4, 5, "Specifies when the evaporatively-precooled condenser for air cooled units can operate"
          EDIT, 13262, 13262, 0, 1, SYSTEM, 0,    EVAP-PCC-ELEC, 0, STD, 565, 105,  23,  50,  6, 3,       "Evap Condenser Electric:", LEFT, -190,  5, 1, LEFT, 4, 5, "Electricity consumption of the evaporative precooling unit"

         LABEL, "Water-Cooled Condenser", STD, LEFT, 360, 160, 1, 0, 0, 655, 13256, 3
          EDIT, 13256, 13256, 0, 1, SYSTEM, 0,     CW-COIL-HEAD, 0, STD, 565, 180,  23,  50,  1, 3,     "Condenser Water Coil Head:", LEFT, -190,  5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the condenser at the design flowrate"
          EDIT, 13257, 13257, 0, 1, SYSTEM, 0,       CW-COIL-DT, 0, STD, 565, 205,  23,  50,  1, 3,  "Condenser Water Coil Delta T:", LEFT, -190,  5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flowrate)"
         COMBO, 13258, 13258, 0, 1, SYSTEM, 0,         CW-VALVE, 0, STD, 500, 230,  85, 150, 19, 3,               "Isolation Valve?", LEFT, -125,  5, 0, LEFT, 4, 5, "Whether an isolation valve regulates flow rate through condenser by cycling with compressor"
         COMBO, 19096, 19096, 0, 1, SYSTEM, 0,          CW-LOOP, 0, STD, 500, 255, 200, 150, 19, 3,                       "CW Loop:", LEFT, -125,  5, 0, LEFT, 4, 5, "If Condenser Type=Water Cooled, CW Loop is required & must be attached to Heat Rejection"


       SUBTABPAGE, 3180, 29031, 1, 3, "  Capacity Curves  "

         LABEL, "f(temperatures)", STD, LEFT, 20,  8, 1, 0, 0, 630, 0, 3
         LABEL, "Total Capacity", STD, CENTER, 235, 22, 1, 0, 0, 0, 0, 3
         COMBO, 13282, 13282, 0, 1, SYSTEM, 0,     COOL-CAP-FT, 0, STD, 165,  40, 200, 145, 19, 3,            "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Bi-Quadratic Curve Fit: Cooling Capacity as a function of entering temperatures"
         LABEL, "t entering drybulb):", STD, LEFT,  46,  52, 1, 0, 0, 0, 13282, 3
;        COMBO, 13283, 13283, 0, 1, SYSTEM, 0,     COOL-CAP-FT, 0, STD, 165,  70, 200, 145, 19, 3,            "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Bi-Quadratic Curve Fit: Cooling Capacity as a function of entering temperatures"
;        LABEL,  "t outdoor drybulb):", STD, LEFT,  46,  82, 1, 0, 0, 0, 13283, 3
; SAC 11/23/10 - removed          
;         COMBO, 13284, 13284, 0, 1, SYSTEM, 0, CHW-CAP-FEWBEWT, 0, STD, 165,  70, 200, 145, 19, 3,            "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Bi-Quadratic eqn: coil capacity as a fct of entering wetbulb temp and entering water temp"
;         LABEL,   "t entering water):", STD, LEFT,  46,  82, 1, 0, 0, 0, 13284, 3
      
         LABEL, "f(flow)", STD, LEFT, 20, 108, 1, 0, 0, 630, 0, 3
         LABEL, "Total Capacity", STD, CENTER, 235, 122, 1, 0, 0, 0, 0, 3
; SAC 11/23/10 - removed          
;         COMBO, 13285, 13285, 0, 1, SYSTEM, 0,     CHW-CAP-FCFM, 0, STD, 165, 140, 200, 145, 19, 3,             "f(supply air flow):", LEFT, -130,  5, 0, LEFT, 4, 5, "Quadratic Equation: chilled water coil capacity as a function of the supply air flow rate"
;        COMBO, 13286, 13286, 0, 1, SYSTEM, 0, RATED-CCAP-FFLOW, 0, STD, 165, 170, 200, 145, 19, 3,           "f(supply/rated flow):", LEFT, -130,  5, 0, LEFT, 4, 5, ""
; SAC 11/23/10 - removed          
;         COMBO, 13287, 13287, 0, 1, SYSTEM, 0,     CHW-CAP-FGPM, 0, STD, 165, 170, 200, 145, 19, 3,                    "f(CHW flow):", LEFT, -130,  5, 0, LEFT, 4, 5, "Quadratic Equation: chilled water coil capacity as a function of the chilled water flow rate"
      
         LABEL, "f(part load)", STD, LEFT, 20, 208, 1, 0, 0, 630, 0, 3
         LABEL, "Total Capacity", STD, CENTER, 235, 222, 1, 0, 0, 0, 0, 3
         COMBO, 13288, 13288, 0, 1, SYSTEM, 0, COOL-CLOSS-FPLR, 0, STD, 165, 240, 200, 145, 19, 3,               "f(cycling on/off):", LEFT, -130,  5, 0, LEFT, 4, 5, "Quadratic Equation: cycling PLR/cycling fraction as a function of cycling PLR"
         COMBO, 13289, 13289, 0, 1, SYSTEM, 0,   COOL-CAP-FRPM, 0, STD, 165, 270, 200, 145, 19, 3,                          "f(RPM):", LEFT, -130,  5, 0, LEFT, 4, 5, "Quadratic Equation: compressor cooling capacity as a function of motor RPM"

         LABEL, "Sensible Capacity", STD, CENTER, 395, 22, 1, 0, 0, 0, 13290, 3
; SAC 11/23/10 - removed          
;         COMBO, 13290, 13290, 0, 1, SYSTEM, 0,      COOL-SH-FT, 0, STD, 325,  40, 200, 145, 19, 3,                                 "", LEFT, -280,  5, 0, LEFT, 4, 5, "B-Quadratic Curve Fit: Sensible Cooling Capacity as a function of entering temperatures"

;        COMBO, 13291, 13291, 0, 1, SYSTEM, 0,      COOL-SH-FT, 0, STD, 325,  70, 200, 145, 19, 3,                                 "", LEFT, -280,  5, 0, LEFT, 4, 5, "B-Quadratic Curve Fit: Sensible Cooling Capacity as a function of entering temperatures"
;        LABEL, "Sensible Capacity", STD, CENTER, 395, 142, 1, 0, 0, 0, 0, 3
;        COMBO, 13292, 13292, 0, 1, SYSTEM, 0,  RATED-SH-FFLOW, 0, STD, 325, 170, 200, 145, 19, 3,                                 "", LEFT, -280,  5, 0, LEFT, 4, 5, ""
      
         LABEL, "Bypass Factor", STD, CENTER, 555,  22, 1, 0, 0, 0, 0, 3
         COMBO, 13293, 13293, 0, 1, SYSTEM, 0,      COIL-BF-FT, 0, STD, 485,  40, 200, 145, 19, 3,                                 "", LEFT, -430,  5, 0, LEFT, 4, 5, "Bi-Quadratic Equation: coil Bypass Factor as a fct of entering air wet-bulb and dry-bulb temps"
; SAC 11/23/10 - removed          
;         LABEL, "Bypass Factor", STD, CENTER, 555, 122, 1, 0, 0, 0, 0, 3
;         COMBO, 13294, 13294, 0, 1, SYSTEM, 0,   COIL-BF-FFLOW, 0, STD, 485, 140, 200, 145, 19, 3,                                 "", LEFT, -430,  5, 0, LEFT, 4, 5, "Cubic Equation: coil Bypass Factor as a function of total supply air flow rate"
         LABEL, "Bypass Factor", STD, CENTER, 555, 222, 1, 0, 0, 0, 0, 3
         COMBO, 13295, 13295, 0, 1, SYSTEM, 0,    COIL-BF-FPLR, 0, STD, 485, 240, 200, 145, 19, 3,                                 "", LEFT, -430,  5, 0, LEFT, 4, 5, "Cubic Equation: coil Bypass Factor as a function of part load ratio"

         EDIT, 13249, 13249, 0, 1, SYSTEM, 0,      COOL-FT-MIN, 0, STD, 230, 305,  23,  40,  1, 3, "Min temp used in cooling curves:", LEFT, -210,  5, 1, LEFT, 4, 5, "Minimum outside air dry bulb temp for which the cooling Curve Fits are valid"


       SUBTABPAGE, 3181, 29032, 1, 3, "  Evaporative Cooling  "

;        for system types RESYS, the following controls apply.
         CASE, SYSTEM, 0, TYPE, -1, =, 1, 17
             LABEL, "Residential Evaporative Cooler", STD, LEFT, 40, 55, 1, 0, 0, 300, 0, 3
             COMBO, 13302, 13302, 0, 1, SYSTEM, 0,  RES-EVAP-COOLER, 0, STD, 215,  75,  85,  85, 19, 3,           "Residential Evap Cooler:", LEFT, -160, 5, 0, LEFT, 4, 5, "Whether a residential system has an add-on (direct) evaporative cooling unit"
              EDIT, 13303, 13303, 0, 1, SYSTEM, 0, RES-EVAP-CL-FLOW, 0, STD, 215, 100,  23,  70,  0, 3,           "Resident Evap Cool Flow:", LEFT, -160, 5, 1, LEFT, 4, 5, "Air side capacity of the residential evaporative cooler (expressed in standard CFM)"
              EDIT, 13304, 13298, 0, 1, SYSTEM, 0,       DIRECT-EFF, 0, STD, 215, 125,  23,  70,  2, 3,              "Direct Effectiveness:", LEFT, -160, 5, 1, LEFT, 4, 5, "Rated (nominal) effectiveness of the direct evaporative cooler"
              EDIT, 13305, 13300, 0, 1, SYSTEM, 0,  EVAP-CL-KW/FLOW, 0, STD, 215, 150,  23,  70,  6, 3,                   "Fan and Pump kW:", LEFT, -160, 5, 1, LEFT, 4, 5, "Power consumption of evaporative cooling pump and secondary fan (per unit air flow)"
         ENDCASE     

;        for system types EVAP-COOLER, the following controls apply.
         CASE, SYSTEM, 0, TYPE, -1, =, 1, 26
;            LABEL, "Stand-Alone Evaporative Cooling", STD, LEFT, 40, 55, 1, 0, 0, 435, 0, 3
;             COMBO, 13296, 13458, 0, 1, SYSTEM, 0,     EVAP-CL-TYPE, 0, STD, 255,  75, 110, 115, 19, 3,           "Evaporative Cooler Type:", LEFT, -200, 5, 0, LEFT, 4, 5, "Type of evaporative cooling element (Direct and/or Indirect or None)"
;             COMBO, 13297, 13297, 0, 1, SYSTEM, 0,   EVAP-CL+REC-RA, 0, STD, 255, 100,  85, 115, 19, 3, "Return Air Used at Indirect Stage:", LEFT, -200, 5, 0, LEFT, 4, 5, "Whether return air is used for the secondary air-stream of the indirect evaporative cooler"
;              EDIT, 13298, 13298, 0, 1, SYSTEM, 0,       DIRECT-EFF, 0, STD, 255, 125,  23,  70,  2, 3,              "Direct Effectiveness:", LEFT, -200, 5, 1, LEFT, 4, 5, "Rated (nominal) effectiveness of the direct evaporative cooler"
;              EDIT, 13299, 13299, 0, 1, SYSTEM, 0,        INDIR-EFF, 0, STD, 255, 150,  23,  70,  2, 3,            "Indirect Effectiveness:", LEFT, -200, 5, 1, LEFT, 4, 5, "Rated (nominal) effectiveness of the indirect evaporative cooler"
;              EDIT, 13300, 13300, 0, 1, SYSTEM, 0,  EVAP-CL-KW/FLOW, 0, STD, 255, 175,  23,  70,  6, 3,           "Pump & Secondary Fan kW:", LEFT, -200, 5, 1, LEFT, 4, 5, "Power consumption of evaporative cooling pump and secondary fan (per unit air flow)"
;;             EDIT, 13301, 13301, 0, 1, SYSTEM, 0,        RECOV-EFF, 0, STD, 255, 200,  23,  60,  2, 3,             "Indirect Recovery Eff:", LEFT, -200, 5, 1, LEFT, 4, 5, ""
;             COMBO, 13931, 13313, 0, 1, SYSTEM, 0, DIRECT-EFF-FFLOW, 0, STD, 255, 200, 300, 180, 19, 3,          "Direct Eff = f(air flow):", LEFT, -200, 5, 0, LEFT, 4, 5, "Cubic eqn: effectiveness of direct evaporative cooling as a function of the air flow"
;             COMBO, 13932, 13317, 0, 1, SYSTEM, 0,  INDIR-EFF-FFLOW, 0, STD, 255, 225, 300, 180, 19, 3,        "Indirect Eff = f(air flow):", LEFT, -200, 5, 0, LEFT, 4, 5, "Cubic eqn: effectiveness of indirect evaporative cooling as a function of the air flow"
; SAC 2/19/09 - replaced above (poorly organized & missing keyword) controls w/ following (better organized & more complete) controls
            LABEL, "Stand-Alone Evaporative Cooling", STD, LEFT, 20, 30, 1, 0, 0, 645, 0, 3
            COMBO, 13296, 13458, 0, 1, SYSTEM, 0,     EVAP-CL-TYPE, 0, STD, 185,  50, 110, 135, 19, 3,                  "Evap Cooler Type:", LEFT, -150, 5, 0, LEFT, 4, 5, "Type of evaporative cooling element (Direct and/or Indirect or None)"
            COMBO, 13297, 13297, 0, 1, SYSTEM, 0,   EVAP-CL+REC-RA, 0, STD, 240,  75,  85,  80, 19, 3, "Return Air Used at Indirect Stage:", LEFT, -205, 5, 0, LEFT, 4, 5, "Whether return air is used for the secondary air-stream of the indirect evaporative cooler"
;            EDIT, 13301, 13301, 0, 1, SYSTEM, 0,        RECOV-EFF, 0, STD, 230, 250,  23,  60,  2, 3,             "Indirect Recovery Eff:", LEFT, -195, 5, 1, LEFT, 4, 5, ""
              
             EDIT, 18983, 18983, 0, 1, SYSTEM, 0,  EVAP-CL-LIMIT-T, 0, STD, 535,  50,  23,  70,  1, 3,                "Drybulb High Limit:", LEFT, -160, 5, 1, LEFT, 4, 5, "Outside air (drybulb) temperature above which the evaporative cooler is turned off"
             EDIT, 13300, 13300, 0, 1, SYSTEM, 0,  EVAP-CL-KW/FLOW, 0, STD, 535,  75,  23,  70,  6, 3,               "Pump & Secondary kW:", LEFT, -160, 5, 1, LEFT, 4, 5, "Power consumption of evaporative cooling pump and secondary fan (per unit air flow)"

            LABEL, "Rating",       STD, CENTER, 215, 118, 1, 0, 0, 0, 13309, 3
            LABEL, "f(air flow)",  STD, CENTER, 345, 134, 1, 0, 0, 0, 13309, 3
             EDIT, 13298, 13298, 0, 1, SYSTEM, 0,       DIRECT-EFF, 0, STD, 185, 150,  23,  60,  2, 3,              "Direct Effectiveness:", LEFT, -150, 5, 1, CENTER, -30, -16, "Rated (nominal) effectiveness of the direct evaporative cooler"
            COMBO, 13931, 13313, 0, 1, SYSTEM, 0, DIRECT-EFF-FFLOW, 0, STD, 260, 150, 300, 180, 19, 3,                                   "", LEFT,   -5, 5, 0, LEFT,     4,   5, "Cubic eqn: effectiveness of direct evaporative cooling as a function of the air flow"
             EDIT, 13299, 13299, 0, 1, SYSTEM, 0,        INDIR-EFF, 0, STD, 185, 175,  23,  60,  2, 3,            "Indirect Effectiveness:", LEFT, -150, 5, 0, LEFT,     4,   5, "Rated (nominal) effectiveness of the indirect evaporative cooler"
            COMBO, 13932, 13317, 0, 1, SYSTEM, 0,  INDIR-EFF-FFLOW, 0, STD, 260, 175, 300, 180, 19, 3,                                   "", LEFT,   -5, 5, 0, LEFT,     4,   5, "Cubic eqn: effectiveness of indirect evaporative cooling as a function of the air flow"
         ENDCASE     
          
;        for system types other than EVAP-COOLER or RESYS, this tab sheet does not apply.
;        CASE, SYSTEM, 0, TYPE, -1, =, 30, 1,2,3,4,5,6,7,8,9,10,11,12,13,14,15,16,18,19,20,21,22,23,24,25,27,28,29,30,31,32
         CASE, ELSE
              LABEL, "Not applicable for systems other than Evaporative Cooler or Residential System", STD, CENTER, 340, 32, 1, 0, 0, 0, 0, 3
              LABEL, "See instead, the Precontioner tab, Add-On Evaporative Cooling subtab",           STD, CENTER, 340, 52, 1, 0, 0, 0, 0, 3
         ENDCASE     
          

       SUBTABPAGE, 3182, 29017, 1, 3, "  Economizer  "

         LABEL, "Water-Side Economizer", STD, LEFT,  40,  30, 1, 0, 0, 405, 13269, 3
         COMBO, 13269, 13269, 0, 1, SYSTEM, 0,         WS-ECONO, 0, STD, 255,  50,  85,  80, 19, 3,         "Water-Side Economizer:", LEFT, -200, 5, 0, LEFT, 4, 5, "Whether or not there is a water side economizer"
          EDIT, 13263, 13263, 0, 1, SYSTEM, 0,    WS-ECONO-XEFF, 0, STD, 255,  75,  23,  50,  2, 3,   "WS Economizer Effectiveness:", LEFT, -200, 5, 1, LEFT, 4, 5, "Design coil effectiveness of heat exchanger between cooling tower water loop and CW loop "
          EDIT, 13264, 13264, 0, 1, SYSTEM, 0,  WS-ECONO-MIN-DT, 0, STD, 255, 100,  23,  50,  1, 3,               "CW Coil Delta T:", LEFT, -200, 5, 1, LEFT, 4, 5, "Minimum delta T between condenser water loop and entering air"
          EDIT, 13265, 13265, 0, 1, SYSTEM, 0,    WSE-COIL-HEAD, 0, STD, 255, 125,  23,  50,  1, 3,    "Water-Side Econo Coil Head:", LEFT, -200, 5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the coil at the design flowrate"
          EDIT, 13266, 13266, 0, 1, SYSTEM, 0,      WSE-COIL-DT, 0, STD, 255, 150,  23,  50,  1, 3, "Water-Side Econo Coil Delta T:", LEFT, -200, 5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flowrate)"
         COMBO, 13267, 13267, 0, 1, SYSTEM, 0,   WSE-VALVE-TYPE, 0, STD, 255, 175,  85, 150, 19, 3,   "Water-Side Econo Valve Type:", LEFT, -200, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
         COMBO, 19097, 19097, 0, 1, SYSTEM, 0,         WSE-LOOP, 0, STD, 255, 200, 300, 150, 19, 3,         "Water-Side Econo Loop:", LEFT, -200, 5, 0, LEFT, 4, 5, "Name of loop that serves the water-side economizer (Loop Type = Chilled Water or 2 Pipe)"
          EDIT, 14520, 14520, 0, 1, SYSTEM, 0,  WS-ECONO-FAN-DT, 0, STD, 255, 225,  23,  50,  2, 3,     "WS Economizer Fan Delta T:", LEFT, -200, 5, 1, LEFT, 4, 5, "Additional fan temperature rise required to overcome air pressure drop thru economizer coil"
          EDIT, 14521, 14521, 0, 1, SYSTEM, 0, WS-ECONO-KW/FLOW, 0, STD, 255, 250,  23,  50,  4, 3,      "Water-Side Economizer kW:", LEFT, -200, 5, 1, LEFT, 4, 5, "Additional fan power required to overcome the air pressure drop through the economizer coil"


; SAC 1/16/06 - added staged volume subtab page from JJH
       SUBTABPAGE, 3363, 29047, 1, 3, "  Staged-Volume  "

        CASE, SYSTEM, 0, TYPE, -1, =, 1, 28
        ;PVVT systems
          COMBO, 17915, 13450, 0, 1, SYSTEM, 0,  AIR/TEMP-CONTROL,0, STD, 240,   5,  80, 145, 19, 3,            "Heating & Cooling Staging Control:", LEFT, -205, 5, 0, LEFT, 4, 5, ""

          LABEL,"Cooling Stages", STD, CENTER, 160,  33, 1, 0, 0, 0, 0, 3

          LABEL,     "Capacity",  STD, CENTER, 125,  49, 1, 0, 0, 0, 0, 3
          LABEL,     "Fraction",  STD, CENTER, 125,  65, 1, 0, 0, 0, 0, 3
         
          LABEL,     "Delta T",   STD, CENTER, 205,  49, 1, 0, 0, 0, 0, 3
          LABEL,     "°F",        STD, CENTER, 205,  65, 1, 0, 0, 0, 0, 3
          
          LABEL,"Heating Stages", STD, CENTER, 320,  33, 1, 0, 0, 0, 0, 3

          LABEL,     "Capacity",  STD, CENTER, 280,  49, 1, 0, 0, 0, 0, 3
          LABEL,     "Fraction",  STD, CENTER, 280,  65, 1, 0, 0, 0, 0, 3
         
          LABEL,     "Delta T",   STD, CENTER, 355,  49, 1, 0, 0, 0, 0, 3
          LABEL,     "°F",        STD, CENTER, 355,  65, 1, 0, 0, 0, 0, 3
         
          LABEL, "Stage 1:", STD, LEFT, 35,  85, 1, 0, 0, 0, 0, 3
          LABEL, "Stage 2:", STD, LEFT, 35, 110, 1, 0, 0, 0, 0, 3
          LABEL, "Stage 3:", STD, LEFT, 35, 135, 1, 0, 0, 0, 0, 3
          LABEL, "Stage 4:", STD, LEFT, 35, 160, 1, 0, 0, 0, 0, 3

          EDIT, 17916, 12306, 0, 1, SYSTEM, 0,  COOL-STAGES    , 0, STD,  90,  80,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" 
          EDIT, 17917, 13066, 0, 1, SYSTEM, 0,  COOL-STAGES    , 1, STD,  90, 105,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17918, 12307, 0, 1, SYSTEM, 0,  COOL-STAGES    , 2, STD,  90, 130,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" 
          EDIT, 17919, 12307, 0, 1, SYSTEM, 0,  COOL-STAGES    , 3, STD,  90, 155,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" 
          
          EDIT, 17920, 13430, 0, 1, SYSTEM, 0,  COOL-STAGES-DT , 0, STD, 175,  80,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17921, 13431, 0, 1, SYSTEM, 0,  COOL-STAGES-DT , 1, STD, 175, 105,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17922, 13432, 0, 1, SYSTEM, 0,  COOL-STAGES-DT , 2, STD, 175, 130,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17923, 13432, 0, 1, SYSTEM, 0,  COOL-STAGES-DT , 3, STD, 175, 155,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
                                                                                                         
          EDIT, 17924, 13433, 0, 1, SYSTEM, 0,  HEAT-STAGES    , 0, STD, 250,  80,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17925, 13434, 0, 1, SYSTEM, 0,  HEAT-STAGES    , 1, STD, 250, 105,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17926, 13435, 0, 1, SYSTEM, 0,  HEAT-STAGES    , 2, STD, 250, 130,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17927, 13435, 0, 1, SYSTEM, 0,  HEAT-STAGES    , 3, STD, 250, 155,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          
          EDIT, 17928, 13436, 0, 1, SYSTEM, 0,  HEAT-STAGES-DT , 0, STD, 325,  80,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17929, 13437, 0, 1, SYSTEM, 0,  HEAT-STAGES-DT , 1, STD, 325, 105,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17930, 13438, 0, 1, SYSTEM, 0,  HEAT-STAGES-DT , 2, STD, 325, 130,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17931, 13438, 0, 1, SYSTEM, 0,  HEAT-STAGES-DT , 3, STD, 325, 155,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""

; SAC 11/24/10 - added
          EDIT, 19234, 19234, 0, 1, SYSTEM, 0,  LOW-FAN-PWR    , 0, STD, 510,  80,  23,  60,  2, 3,          "Low Fan Power:", LEFT, -95, 5, 1, LEFT, 4, 5, "Fan power ratio when running on low speed"
        ENDCASE 
        CASE, SYSTEM, 0, TYPE, -1, =, 31, 1,2,3,4,5,6,7,8,9,10,11,12,13,14,15,16,17,18,19,20,21,22,23,24,25,26,27,29,30,31,32
        ;everthing except PVVT
          LABEL, "Staged Volume and 2-speed parameters apply only to PVVT systems", STD, LEFT, 20,  15, 1, 0, 0, 0, 0, 3
        ENDCASE 


    ;*****************************************
    ; Heating
    ;*****************************************
    TABPAGE, 3056, 10245, 1, 3, NOTIMP, "  Heating  "
    
;  RADIOFIRST, 29042, 29042, 0, 1, 0, PowerDOE, 0, SysModeHeating,    0, 0, STD,  17, 14,  18,  95, 3, 
;  RADIONEXT,  29043, 29043, 0, 1, 0, PowerDOE, 0, SysModeHeating2,   0, 1, STD, 119, 14,  18,  90, 3, 
;  RADIONEXT,  29044, 29044, 0, 1, 0, PowerDOE, 0, SysModeHeating3,   0, 2, STD, 216, 14,  18, 100, 3, 
;  RADIONEXT,  29045, 29045, 0, 1, 0, PowerDOE, 0, SysModeHeating4,   0, 3, STD, 323, 14,  18, 110, 3, 
;  RADIONEXT,  29049, 29049, 0, 1, 0, PowerDOE, 0, SysModeHeating5,   0, 4, STD, 439, 14,  18, 150, 3, 

       SUBTABPAGE, 3183, 29042, 1, 3, " Coil Cap / Control "

         LABEL, "Heating Capacity", STD, LEFT, 20, 10, 1, 0, 0, 325, 0, 3
         COMBO, 13386, 13489, 0, 1, SYSTEM, 0,       HEAT-SOURCE, 0, STD, 175,   30, 190, 150, 19, 3,                   "Heat Source:", LEFT, -140,  5, 0, LEFT, 4, 5, "The source of heat for the main heating coils (in the central air distribution system)"
         COMBO, 13389, 13389, 0, 1, SYSTEM, 0,  ZONE-HEAT-SOURCE, 0, STD, 175,   55, 190, 150, 19, 3,              "Zone Heat Source:", LEFT, -140,  5, 0, LEFT, 4, 5, "Heat source for the zonal (reheat) coils for all zones in the system"
          EDIT, 13385, 12275, 0, 1, SYSTEM, 0,  HEATING-CAPACITY, 0, STD, 175,   80,  23, 115,  0, 3,              "Heating Capacity:", LEFT, -140,  5, 1, LEFT, 4, 5, "Heating capacity (ar ARI conditions) of the system heating HVAC system"
; DEM 02/22/16 - new keywords
         COMBO, 19342, 19342, 0, 1, SYSTEM, 0,  HT-SIZING-METHOD, 0, STD, 200,  105, 190, 130, 19, 3,              "Central Heat Sizing Method:", LEFT, -165,  5, 0, LEFT, 4, 5, "Method for sizing central heating coil"
          EDIT, 19345, 19345, 0, 1, SYSTEM, 0,    HT-COIL-AIR-DT, 0, STD, 200,  130,  23, 50,  0, 3,              "Heating Coil Air DT:", LEFT, -165,  5, 1, LEFT, 4, 5, "Temperature rise of air through heating coil at design conditions"
         COMBO, 19343, 19343, 0, 1, SYSTEM, 0,  RHT-SIZING-METHO, 0, STD, 200,  155, 190, 130, 19, 3,              "Reheat Coil Sizing Method:", LEFT, -165,  5, 0, LEFT, 4, 5, "Method for sizing zonal (reheat) coils for all zones in the system"

; SAC 11/23/10 - added
         LABEL, "Rated Entering Temps:", STD, LEFT, 35, 200, 1, 0, 0, 0, 19214, 3
          EDIT, 19217, 19217, 0, 1, SYSTEM, 0,      HT-RATED-EDB, 0, STD, 175, 195,  23,  45,  1, 3,                          "DBT", CENTER, 23, -15, 0, LEFT, 4, 5, "The indoor entering drybulb corresponding to the heating capacity"
          EDIT, 19218, 19218, 0, 1, SYSTEM, 0,      HT-RATED-ECT, 0, STD, 225, 195,  23,  45,  1, 3,                        "Cond.", CENTER, 23, -15, 1, LEFT, 4, 5, "The entering 'condenser' temperature corresponding to the heating capacity"

          EDIT, 13384, 13479, 0, 1, SYSTEM, 0,  HEAT-SIZING-RATI, 0, STD, 220, 220,  23,  50,  2, 3,             "Heat Sizing Ratio:", LEFT, -185,  5, 1, LEFT, 4, 5, "Used to deliberately oversize or undersize heating coil capacity when autosizing"

; SAC 11/23/10 - added
          EDIT, 19219, 19219, 0, 1, SYSTEM, 0,     HEAT/COOL-CAP, 0, STD, 220, 245,  23,  50,  2, 3,      "Heat/Cool Capacity Ratio:", LEFT, -185,  5, 1, LEFT, 4, 5, "For a heat pump, is the ratio of the heating capacity to the cooling capacity"

          EDIT, 13400, 13400, 0, 1, SYSTEM, 0,    HEAT-CLOSS-MIN, 0, STD, 220, 270,  23,  50,  2, 3,   "Min Cycling Part Load Ratio:", LEFT, -185,  5, 1, LEFT, 4, 5, "Min cycling PLR for which the Total Heating Capacity f(PLR) operating curve is valid"
          EDIT, 13401, 13401, 0, 1, SYSTEM, 0,      HW-COIL-HEAD, 0, STD, 220, 295,  23,  50,  1, 3,           "Hot Water Coil Head:", LEFT, -185,  5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the coil at the design flowrate"
          EDIT, 13404, 13404, 0, 1, SYSTEM, 0,        HW-COIL-DT, 0, STD, 220, 320,  23,  50,  1, 3,        "Hot Water Coil Delta T:", LEFT, -185,  5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flowrate)"

         LABEL, "Heating Control and Reset", STD, LEFT, 365, 10, 1, 0, 0, 650, 0, 3
          EDIT, 13373, 12269, 0, 1, SYSTEM, 0,      MAX-SUPPLY-T, 0, STD, 580,  30,  23,  50,  1, 3, "Zone Entering Max Supply Temp:", LEFT, -200,  5, 1, LEFT, 4, 5, ""
          EDIT, 13374, 13482, 0, 1, SYSTEM, 0,        HEAT-SET-T, 0, STD, 580,  55,  23,  50,  1, 3,     "Hot Deck Max Leaving Temp:", LEFT, -200,  5, 1, LEFT, 4, 5, "Maximum allowable temperature setpoint of the central heating coil"
          EDIT, 13375, 13483, 0, 1, SYSTEM, 0,    REHEAT-DELTA-T, 0, STD, 555,  80,  23,  50,  1, 3,                "Reheat Delta T:", LEFT, -175,  5, 1, LEFT, 4, 5, "Maximum increase in supply air temperature due to system reheat coils"
; removed to make room for ZONE-HW-LOOP combo
;         EDIT, 13376, 13484, 0, 1, SYSTEM, 0,      MIN-HUMIDITY, 0, STD, 580, 105,  23,  40,  1, 3,              "Minimum Humidity:", LEFT, -200,  5, 1, LEFT, 4, 5, "Lowest allowable relative humidity in the return air (from all zones served by the system)"
;        COMBO, 13377, 13159, 0, 1, SYSTEM, 0,   HUMIDIFIER-TYPE, 0, STD, 490, 130, 190, 150, 19, 3,               "Humidifier Type:", LEFT, -110,  5, 0, LEFT, 4, 5, "The heat source for humidification in the central air distribution system"
         LABEL, "RPM Limits:", STD, LEFT, 380, 110, 1, 0, 0, 0, 13388, 3
          EDIT, 13388, 13388, 0, 1, SYSTEM, 0,   HEAT-RPM-LIMITS, 0, STD, 555, 105,  23,  75,  0, 3,                       "Maximum:", RIGHT,  -5,  5, 1, LEFT, 4, 5, "Maximum allowable speed (RPM) of the heat pump engine during heating"
          EDIT, 13387, 13387, 0, 1, SYSTEM, 0,   HEAT-RPM-LIMITS, 1, STD, 555, 130,  23,  75,  0, 3,                       "Minimum:", RIGHT,  -5,  5, 1, LEFT, 4, 5, "Minimum allowable speed (RPM) of the heat pump engine during heating"
         COMBO, 13378, 13378, 0, 1, SYSTEM, 0,      HEAT-SET-SCH, 0, STD, 490, 155, 200, 160, 19, 3,                "Hot Deck Sched:", LEFT, -110,  5, 0, LEFT, 4, 5, "Temperature of the heating supply air temperature (used only if Heating Control = Scheduled)"
         COMBO, 13379, 13485, 0, 1, SYSTEM, 0,  HEATING-SCHEDULE, 0, STD, 490, 180, 200, 160, 19, 3,              "Availability Sch:", LEFT, -110,  5, 0, LEFT, 4, 5, "Whether mechanical heating is allowed"
         COMBO, 13380, 13486, 0, 1, SYSTEM, 0,      HEAT-CONTROL, 0, STD, 490, 205, 120, 160, 19, 3,                  "Heat Control:", LEFT, -110,  5, 0, LEFT, 4, 5, "Strategy used to control supply air temperature leaving the systems central heating coil"
         COMBO, 13381, 13381, 0, 1, SYSTEM, 0,    HEAT-RESET-SCH, 0, STD, 490, 230, 200, 160, 19, 3,                "Heat Reset Sch:", LEFT, -110,  5, 0, LEFT, 4, 5, "A Reset Temp Schedule that defines the heating supply air temp as a fct of outside air temp"
          EDIT, 13383, 13383, 0, 1, SYSTEM, 0,  HEAT-MIN-RESET-T, 0, STD, 580, 255,  23,  50,  1, 3,    "Minimum Heating Reset Temp:", LEFT, -200,  5, 1, LEFT, 4, 5, "Minimum temperature that the supply air temperature can be reset to during heating"
; SAC 11/23/10 - added
          EDIT, 19220, 19220, 0, 1, SYSTEM, 0,  HEAT-MAX-RESET-T, 0, STD, 580, 280,  23,  50,  1, 3,    "Maximum Heating Reset Temp:", LEFT, -200,  5, 1, LEFT, 4, 5, "Maximum temperature to which the supply air temperature resets during Heat Control = Coldest"

         COMBO, 13382, 13382, 0, 1, SYSTEM, 0,  HCOIL-WIPE-FFLOW, 0, STD, 505, 305, 200, 145, 19, 3,            "Heating Coil Wipe =", LEFT, -125, -4, 0, LEFT, 4, 5, ""
         LABEL, "f(cooling flow):", STD,RIGHT, 500, 317, 1, 0, 0, 0, 13382, 3

; DEM 02/22/16 Moved to upper right of form
         LABEL, "Loops and Attachments", STD, LEFT, 680, 10, 1, 0, 0, 965, 0, 3
         COMBO, 13402, 13402, 0, 1, SYSTEM, 0,     HW-VALVE-TYPE, 0, STD, 800, 30,  85, 150, 19, 3,                 "HW Valve Type:", LEFT, -120,  5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
         COMBO, 19098, 19098, 0, 1, SYSTEM, 0,           HW-LOOP, 0, STD, 800, 55, 200, 150, 19, 3,                       "HW Loop:", LEFT, -120,  5, 0, LEFT, 4, 5, "Name of loop that serves the system hot water coils (Loop Type = Hot Water or Two Pipe)"
         COMBO, 19139, 19139, 0, 1, SYSTEM, 0,          DHW-LOOP, 0, STD, 800, 80, 200, 150, 19, 3,                      "DHW Loop:", LEFT, -120,  5, 0, LEFT, 4, 5, "Name of the Loop that provides Domestic Hot Water to the zones in this system"
         COMBO, 14600, 14600, 0, 1, SYSTEM, 0,      ZONE-HW-LOOP, 0, STD, 800, 105, 200, 150, 19, 3,                  "Zone HW Loop:", LEFT, -120,  5, 0, LEFT, 4, 5, ""
; DEM: CHANGE1
; SAC 11/23/10 - added 
; DEM 10/25/16 moved to new tab
;         COMBO, 19221, 19221, 0, 1, SYSTEM, 0,   CONDENSING-UNIT, 0, STD, 800, 130, 200, 150, 19, 3,               "Condensing Unit:", LEFT, -120,  5, 0, LEFT, 4, 5, "The U-name of a CONDENSING-UNIT to which the cooling/heating coil(s) in this system are connected"
;         COMBO, 19222, 19222, 0, 1, SYSTEM, 0,  HEAT/COOL-CONFIG, 0, STD, 840, 155, 200, 110, 19, 3,       "Heat/Cool Configuration:", LEFT, -160,  5, 0, LEFT, 4, 5, "If both heating and cooling coils attached to a condensing-unit, whether a common coil"
;         COMBO, 19223, 19223, 0, 1, SYSTEM, 0,     RFG-COIL-CTRL, 0, STD, 840, 180, 200, 110, 19, 3,             "Refg Coil Control:", LEFT, -160,  5, 0, LEFT, 4, 5, "For condensing unit, specifies how the coil is controlled in response to the zone thermostat or discharge air controller"

       SUBTABPAGE, 3184, 29043, 1, 3, " Unitary Power "

         LABEL, "Heating Electric Power", STD, LEFT, 20, 15, 1, 0, 0, 330, 13405, 3
          EDIT, 13405, 12384, 0, 1, SYSTEM, 0,      HEATING-EIR, 0, STD, 205,  40,  23,  80,  4, 3, "Heating Electric Input Ratio:", LEFT, -170,  5, 1, LEFT, 4, 5, ""
;         EDIT, 13406, 14513, 0, 1, SYSTEM, 0,   UNIT-PUMP-ELEC, 0, STD, 205,  ??,  23,  80,  4, 3,           "Unit Pump Electric:", LEFT, -170,  5, 1, LEFT, 4, 5, "Pump power for the Gas Heat Pump, or supplemental boiler (per Btu Cooling Capacity)"
;         EDIT, 13407, 14514, 0, 1, SYSTEM, 0,      UNIT-AUX-KW, 0, STD, 205,  ??,  23,  80,  2, 3,         "Unit Auxiliary Power:", LEFT, -170,  5, 1, LEFT, 4, 5, "Power consumption of Gas Heat Pump's auxiliaries (e.g., controls), that operate continuously"

         LABEL, "Furnace", STD, LEFT, 20,  75, 1, 0, 0, 330, 0, 3
          EDIT, 13408, 13408, 0, 1, SYSTEM, 0,      FURNACE-HIR, 0, STD, 205, 100,  23,  80,  4, 3,     "Furnace Heat Input Ratio:", LEFT, -170,  5, 1, LEFT, 4, 5, "The ratio of fuel energy consumption to heating energy produced"
          EDIT, 13409, 13409, 0, 1, SYSTEM, 0,      FURNACE-AUX, 0, STD, 205, 125,  23,  80,  1, 3,       "Furnace Fuel Auxiliary:", LEFT, -170,  5, 1, LEFT, 4, 5, "For oil furnaces, aux consumed when furnace has load; for gas, consumed when no load"
          EDIT, 13410, 13410, 0, 1, SYSTEM, 0,   FURNACE-AUX-KW, 0, STD, 205, 150,  23,  80,  2, 3,   "Furnace Electric Auxiliary:", LEFT, -170,  5, 1, LEFT, 4, 5, "Electrical auxiliary power consumed by the furnace when it is on"
         COMBO, 13411, 13411, 0, 1, SYSTEM, 0, FURNACE-HIR-FPLR, 0, STD, 170, 175, 300, 135, 19, 3,         "Furnace HIR = f(plr):", LEFT, -135,  5, 0, LEFT, 4, 5, "Cubic Curve Fit: the Heat Input Ratio as a function of the part load ratio"
         COMBO, 13412, 13412, 0, 1, SYSTEM, 0, FURNACE-OFF-LOSS, 0, STD, 170, 200, 300, 135, 19, 3,             "Furnace Off Loss:", LEFT, -135,  5, 0, LEFT, 4, 5, "Cubic equation:fraction of unused furnace capacity that's an induced load as fct of OA drybulb"
         

; AFR 7/15/09 - moved here from Compliance/Fans
          EDIT, 15577, 15577, 0, 1, SYSTEM, 0,   C-TOTAL-HTG-CAP, 0, STD, 170, 240,  23,  95,  1, 7,           "Total Heating Capacity:", LEFT, -145, 5, 1, LEFT, 4, 5, "The total heating capacity of all identical units"
          EDIT, 15581, 15581, 0, 1, SYSTEM, 0,  C-USER-INPUT-HIR, 0, STD, 520, 240,  23,  80,  3, 7,  "Pre-calculated Heat Input Ratio:", RIGHT,  -8, 5, 1, LEFT, 4, 5, "The user calculated HIR for multiple furnaces simulated as one system"

         LABEL, "Efficiency Ratings:", STD, LEFT,  25, 280, 1, 0, 0, 310, 0, 7
         LABEL, "FULL LOAD",           STD, LEFT, 320, 280, 1, 0, 0, 520, 0, 7
         LABEL, "PART LOAD",           STD, LEFT, 530, 280, 1, 0, 0, 640, 0, 7

         LABEL, "Seasonal Furnace Ratings:",            STD, LEFT,  25, 305, 1, 0, 0, 0, 15578, 7
         LABEL, "Furnace Ratings:",                     STD, LEFT,  25, 330, 1, 0, 0, 0, 15579, 7
         LABEL, "Seasonal Heat Pump Ratings:",          STD, LEFT,  25, 355, 1, 0, 0, 0, 15565, 7
         LABEL, "Air-Cooled Heat Pump Ratings:",        STD, LEFT,  25, 380, 1, 0, 0, 0, 15563, 7
         LABEL, "Water/Grnd Source Ht Pump Ratings:",   STD, LEFT,  25, 405, 1, 0, 0, 0, 15571, 7

          EDIT, 15578, 15578, 0, 1, SYSTEM, 0,            C-AFUE, 0, STD, 310, 305,  23,  80,  2, 7,                        "AFUE:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The AFUE of the furnace"
          EDIT, 15579, 15579, 0, 1, SYSTEM, 0,   C-THERM-EFF-MAX, 0, STD, 310, 330,  23,  80,  2, 7,                      "Et Max:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The thermal efficiency of the furnace at its maximum capacity"
          EDIT, 15580, 15580, 0, 1, SYSTEM, 0,   C-THERM-EFF-MIN, 0, STD, 520, 330,  23,  80,  2, 7,                      "Et Min:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The thermal efficiency of the furnace at its minimum capacity"
          EDIT, 15565, 15565, 0, 1, SYSTEM, 0,            C-HSPF, 0, STD, 310, 355,  23,  80,  2, 7,                        "HSPF:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The HSPF of the heat pump"
          EDIT, 15563, 15563, 0, 1, SYSTEM, 0,           C-COP47, 0, STD, 310, 380,  23,  80,  2, 7,                      "COP 47:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The COP at 47F (ODB) of the air cooled heat pump"
          EDIT, 15564, 15564, 0, 1, SYSTEM, 0,           C-COP17, 0, STD, 520, 380,  23,  80,  2, 7,                      "COP 17:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The COP at 17F (ODB) of the air cooled heat pump"
          EDIT, 15571, 15571, 0, 1, SYSTEM, 0,        C-COP70EWT, 0, STD, 310, 405,  23,  80,  2, 7,                      "COP 70:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The COP at 70F (EWT) of the ground source heat pump"
          EDIT, 15572, 15572, 0, 1, SYSTEM, 0,        C-COP50EWT, 0, STD, 520, 405,  23,  80,  2, 7,                      "COP 50:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The COP at 50F (EWT) of the ground source heat pump"


         LABEL, "Heating Electric Input Ratio Curves", STD, LEFT, 370,  15, 1, 0, 0, 655, 0, 3
         COMBO, 13413, 13413, 0, 1, SYSTEM, 0,      HEAT-EIR-FT, 0, STD, 515,  40, 300, 140, 19, 3,         "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Quadratic Curve Fit: EIR as a function of temp of entering water & outdoor drybulb"
         LABEL, "t outdoor drybulb):", STD, LEFT, 396,  52, 1, 0, 0, 0, 13413, 3
;        COMBO, 13414, 13414, 0, 1, SYSTEM, 0,      HEAT-EIR-FT, 0, STD, 515,  ??, 300, 140, 19, 3,         "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Quadratic Curve Fit: Electric Input Ratio as a function of temperature entering & leaving water"
;        LABEL, "t entering water):", STD, LEFT, 396, 119, 1, 0, 0, 0, 0, 3
;        COMBO, 13415, 13415, 0, 1, SYSTEM, 0, RATED-HEIR-FFLOW, 0, STD, 515, ???, 300, 140, 19, 3,         "f(supply/rated flow):", LEFT, -130,  5, 0, LEFT, 4, 5, ""
         COMBO, 13416, 13416, 0, 1, SYSTEM, 0,    HEAT-EIR-FPLR, 0, STD, 515,  70, 300, 140, 19, 3,           "f(part load ratio):", LEFT, -130,  5, 0, LEFT, 4, 5, "Cubic Curve Fit: Electric Input Ratio as a function of the part load ratio"
         COMBO, 13417, 13417, 0, 1, SYSTEM, 0,    HEAT-EIR-FRPM, 0, STD, 515, 100, 300, 140, 19, 3,                       "f(RPM):", LEFT, -130,  5, 0, LEFT, 4, 5, "Cubic Curve Fit: Electric Input Ratio as a function of heat pump engine RPM"

         LABEL, "Gas Heat Pump Auxiliary Electric", STD, LEFT, 370, 150, 1, 0, 0, 615, 13406, 3
         EDIT, 13406, 14513, 0, 1, SYSTEM, 0, UNIT-PUMP-ELEC, 0, STD, 515, 175,  23,  60,  3, 3,                  "Gas HP Pump kW:", LEFT, -130,  5, 1, LEFT, 4, 5, "Pump power for the Gas Heat Pump, or supplemental boiler (per Btu Cooling Capacity)"
         EDIT, 13407, 14514, 0, 1, SYSTEM, 0,    UNIT-AUX-KW, 0, STD, 515, 200,  23,  60,  3, 3,                   "Gas HP Aux kW:", LEFT, -130,  5, 1, LEFT, 4, 5, "Power consumption of Gas Heat Pump's auxiliaries (e.g., controls), that operate continuously"

; AFR 7/15/09 - moved to upper right
         LABEL, "Low Speed Electric Input Ratio Curve", STD, LEFT, 680, 15, 1, 0, 0, 655, 13418, 3
         COMBO, 13418, 13418, 0, 1, SYSTEM, 0,   HEAT-EIR-LS-FT, 0, STD, 825, 40, 300, 140, 19, 3,         "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Bi-Quadratic eqn: heating EIR (at min RPM) as fct of entering air wetbulb and OA drybulb"
         LABEL, "t outdoor drybulb):", STD, LEFT, 706, 52, 1, 0, 0, 0, 13418, 3


       SUBTABPAGE, 3185, 29044, 1, 3, " Preht / Basebrd "

         LABEL, "Preheat", STD, LEFT, 20, 30, 1, 0, 0, 295, 12604, 3
         COMBO, 12604, 12604, 0, 1, SYSTEM, 0,   PREHEAT-SOURCE, 0, STD, 175,  50, 190, 120, 19, 3,         "Preheat Source:", LEFT, -140, 5, 0, LEFT, 4, 5, "The source of heat the preheat coils in the central air distribution system"
; DEM 11/28/16 - new keyword
         COMBO, 19480, 19480, 0, 1, SYSTEM, 0,     PREHEAT-LOCN, 0, STD, 175,  75, 190, 120, 19, 3,       "Preheat Location:", LEFT, -140, 5, 0, LEFT, 4, 5, "Location of preheat coil"
; DEM 02/22/16 - new keyword
         COMBO, 19344, 19344, 0, 1, SYSTEM, 0, PHT-SIZING-METHO, 0, STD, 175, 100, 190, 120, 19, 3,  "Preheat Sizing Method:", LEFT, -140, 5, 0, LEFT, 4, 5, "Method for sizing preheat coil"
          EDIT, 19346, 19346, 0, 1, SYSTEM, 0,   PHT-COIL-AIR-DT, 0, STD, 175, 125,  23, 50,  0, 3,    "Preheat Coil Air DT:", LEFT, -140,  5, 1, LEFT, 4, 5, "Temperature rise of air through preheat coil at design conditions"
          EDIT, 12519, 12519, 0, 1, SYSTEM, 0, PREHEAT-CAPACITY, 0, STD, 175, 150,  23,  90,  0, 3,       "Preheat Capacity:", LEFT, -140, 5, 1, LEFT, 4, 5, "Total capacity of the preheat coil at the design conditions"
; SAC 11/23/10 - added
; TWV 11/28/11 - replace PREHEAT-FLOW with PHT-RATED-FLOW, no longer included in BDLKey.out
          EDIT, 19224, 19224, 0, 1, SYSTEM, 0,   PHT-RATED-FLOW, 0, STD, 175, 175,  23,  90,  0, 3,           "Preheat Flow:", LEFT, -140, 5, 1, LEFT, 4, 5, "The airflow corresponding to the Preheat Capacity"
          EDIT, 19225, 19225, 0, 1, SYSTEM, 0,    PHT-RATED-EDB, 0, STD, 215, 200,  23,  50,  1, 3, "Rated Entering Drybulb:", LEFT, -180, 5, 1, LEFT, 4, 5, "The entering drybulb temperature corresponding to the Preheat Capacity"

          EDIT, 12572, 13490, 0, 1, SYSTEM, 0,        PREHEAT-T, 0, STD, 215, 225,  23,  50,  1, 3,   "Preheat Leaving Temp:", LEFT, -180, 5, 1, LEFT, 4, 5, "Minimum temperature of the air leaving the preheat coil"
          EDIT, 12620, 12620, 0, 1, SYSTEM, 0,    PHW-COIL-HEAD, 0, STD, 215, 250,  23,  50,  1, 3,          "PHW Coil Head:", LEFT, -180, 5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the preheat coil at the design flow rate"
          EDIT, 12637, 12637, 0, 1, SYSTEM, 0,      PHW-COIL-DT, 0, STD, 215, 275,  23,  50,  1, 3,       "PHW Coil Delta T:", LEFT, -180, 5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flowrate)"
         COMBO, 12653, 12653, 0, 1, SYSTEM, 0,   PHW-VALVE-TYPE, 0, STD, 155, 300,  85, 140, 19, 3,         "PHW Valve Type:", LEFT, -120, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
         COMBO, 19099, 19099, 0, 1, SYSTEM, 0,         PHW-LOOP, 0, STD, 155, 325, 200, 140, 19, 3,               "PHW Loop:", LEFT, -120, 5, 0, LEFT, 4, 5, "Name of the loop to which the system's central preheat coil is connected"
         
         LABEL, "Baseboards", STD, LEFT, 350, 30, 1, 0, 0, 645, 12685, 3
         COMBO, 12685, 13488, 0, 1, SYSTEM, 0, BASEBOARD-SOURCE, 0, STD, 495,  50, 190, 150, 19, 3,       "Baseboard Source:", LEFT, -130, 5, 0, LEFT, 4, 5, "The source of heat for the baseboard heaters (for all zones in the system)"
         COMBO, 12701, 12701, 0, 1, SYSTEM, 0,    BASEBOARD-SCH, 0, STD, 495,  75, 200, 150, 19, 3,        "Baseboard Sched:", LEFT, -130, 5, 0, LEFT, 4, 5, "A Reset Temp Schedule that defines baseboard heat output as fct of outside air temperature "
          EDIT, 12718, 12718, 0, 1, SYSTEM, 0,   BBRD-COIL-HEAD, 0, STD, 570, 100,  23,  50,  1, 3,    "Baseboard Coil Head:", LEFT, -205, 5, 1, LEFT, 4, 5, "Pressure drop of the loop fluid through the baseboards at the design flowrate"
          EDIT, 13098, 13098, 0, 1, SYSTEM, 0,     BBRD-COIL-DT, 0, STD, 570, 125,  23,  50,  1, 3,      "Baseboard Delta T:", LEFT, -205, 5, 1, LEFT, 4, 5, "Temperature change through the coil at design conditions (used to calculate design flowrate)"
         COMBO, 13147, 13147, 0, 1, SYSTEM, 0,  BBRD-VALVE-TYPE, 0, STD, 515, 150,  85, 130, 19, 3,   "Baseboard Valve Type:", LEFT, -150, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
         COMBO, 19100, 19100, 0, 1, SYSTEM, 0,        BBRD-LOOP, 0, STD, 495, 175, 200, 150, 19, 3,         "Baseboard Loop:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of loop that serves baseboard coils (Loop Type must be Hot Water, 2Pipe or Steam)"


       SUBTABPAGE, 3186, 29045, 1, 3, " Supp Heat/Defrost "

         LABEL, "Supplemental Heat", STD, LEFT, 20, 30, 1, 0, 0, 295, 13200, 3
         COMBO, 13200, 13200, 0, 1, SYSTEM, 0,   HP-SUPP-SOURCE, 0, STD, 165,  50, 190, 130, 19, 3,               "HP Supp Source:", LEFT, -130,  5, 0, LEFT, 4, 5, "The source of heat for the heat pump's supplemental heating"
          EDIT, 13193, 13193, 0, 1, SYSTEM, 0,   HP-SUPP-HT-CAP, 0, STD, 185,  75,  23,  80,  0, 3,        "HP Supp Heat Capacity:", LEFT, -150,  5, 1, LEFT, 4, 5, "Supplemental heating capacity of a heat pump"
          EDIT, 13230, 13230, 0, 1, SYSTEM, 0,         MIN-HP-T, 0, STD, 215, 100,  23,  50,  1, 3,         "Minimum HP Heat Temp:", LEFT, -180,  5, 1, LEFT, 4, 5, "Outside air (drybulb) temperature below which the heat pump is turned off"
          EDIT, 13231, 13231, 0, 1, SYSTEM, 0,    MAX-HP-SUPP-T, 0, STD, 215, 125,  23,  50,  1, 3,         "Maximum HP Supp Temp:", LEFT, -180,  5, 1, LEFT, 4, 5, "Outside air drybulb temp below which heat pump supplemental heating is allowed"
; SAC 11/23/10 - removed          
;          EDIT, 13232, 13232, 0, 1, SYSTEM, 0, RESIST-CAP-RATIO, 0, STD, 215, 150,  23,  50,  2, 3, "Resistive Cap / HP Cap Ratio:", LEFT, -180,  5, 1, LEFT, 4, 5, "Ratio of the default return (relief) fan capacity to the supply capacity"
         
         LABEL, "Defrost", STD, LEFT, 340, 30, 1, 0, 0, 650, 13237, 3
         COMBO, 13237, 13237, 0, 1, SYSTEM, 0,     DEFROST-TYPE, 0, STD, 505,  50,  85, 145, 19, 3,                 "Defrost Type:", LEFT, -150,  5, 0, LEFT, 4, 5, "Whether heat pump is defrosted via electric resistance coils or a reverse cycle"
         COMBO, 13238, 13238, 0, 1, SYSTEM, 0,     DEFROST-CTRL, 0, STD, 505,  75,  85, 145, 19, 3,              "Defrost Control:", LEFT, -150,  5, 0, LEFT, 4, 5, "The defrost control method for the heat pump "
          EDIT, 13239, 13239, 0, 1, SYSTEM, 0,        DEFROST-T, 0, STD, 580, 100,  23,  50,  1, 3,  "Maximum Defrost Temperature:", LEFT, -225,  5, 1, LEFT, 4, 5, "Outdoor air drybulb temp below which heat pump defrosts itself (when in the heating mode)"
         COMBO, 13240, 13240, 0, 1, SYSTEM, 0,  DEFROST-FRAC-FT, 0, STD, 505, 150, 200, 145, 19, 3,        "Defrost Runtime Frac =", LEFT, -150, -4, 0, LEFT, 4, 5, "Bi-Quadratic eqn: defrost run time fraction as a fct of outside air wetbulb and drybulb temps"
         LABEL, "f(outdoor drybulb, wb):", STD, LEFT, 366, 162, 1, 0, 0, 0, 13240, 3

;        COMBO, 13241, 13241, 0, 1, SYSTEM,  0,  DEFROST-CAP-FT, 0, STD, 455, 185, 200, 130, 19, 3,            "Defrost Capacity =", LEFT, -150, -4, 0, LEFT, 4, 5, ""
;        LABEL,     "f(outdoor wetbulb):", STD, LEFT, 305, 193, 1, 0, 0, 0, 0, 3
;        COMBO, 13242, 13242, 0, 1, SYSTEM,  0,  DEFROST-PWR-FT, 0, STD, 455, 215, 200, 130, 19, 3,               "Defrost Power =", LEFT, -150, -4, 0, LEFT, 4, 5, ""
;        LABEL,    "f(outdoor, wetbulb):", STD, LEFT, 305, 223, 1, 0, 0, 0, 0, 3


       SUBTABPAGE, 3187, 29049, 1, 3, " Cap Curves/Waste Ht "

         LABEL, "Total Capacity as f(temperatures)", STD,   LEFT,  20, 10, 1, 0, 0, 305, 0, 3
         COMBO, 13245, 13245, 0, 1, SYSTEM, 0,      HEAT-CAP-FT, 0, STD, 165,  35, 200, 140, 19, 3,            "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Bi-Quadratic eqn: Heating Capacity of heat pump as fct of OA drybulb & entering air drybulb"
         LABEL, "t entering drybulb):",  STD,   LEFT,  46,  47, 1, 0, 0, 0, 13245, 3
;        COMBO, 13390, 13390, 0, 1, SYSTEM, 0,      HEAT-CAP-FT, 0, STD, 165,  ??, 200, 140, 19, 3,            "f(t entering wetbulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Bi-Quadratic eqn: Heating Capacity of heat pump as fct of OA drybulb & entering air wetbulb"
;        LABEL, "t entering wetbulb):",  STD,   LEFT,  46, ???, 1, 0, 0, 0, 0, 3
; SAC 11/23/10 - removed          
;         COMBO, 13391, 13391, 0, 1, SYSTEM, 0,       HW-CAP-FDT, 0, STD, 165,  65, 200, 140, 19, 3,            "f(t entering drybulb,", LEFT, -130, -4, 0, LEFT, 4, 5, "Quadratic eqn: coil capacity as fct of temp difference between entering air and entering water"
;         LABEL,   "t entering water):",  STD,   LEFT,  46,  77, 1, 0, 0, 0, 13391, 3
         
         LABEL, "Total Capacity as f(flow)", STD,   LEFT,  20, 100, 1, 0, 0, 305, 0, 3
; SAC 11/23/10 - removed          
;         COMBO, 13392, 13392, 0, 1, SYSTEM, 0,      HW-CAP-FCFM, 0, STD, 155, 125, 200, 150, 19, 3,              "f(supply air flow):", LEFT, -120,  5, 0, LEFT, 4, 5, "Quadratic eqn: coil capacity as a function of supply air flow rate"
;        COMBO, 13393, 13393, 0, 1, SYSTEM, 0, RATED-HCAP-FFLOW, 0, STD, 155, ???, 200, 150, 19, 3,            "f(supply/rated flow):", LEFT, -120,  5, 0, LEFT, 4, 5, ""
; SAC 11/23/10 - removed          
;         COMBO, 13394, 13394, 0, 1, SYSTEM, 0,      HW-CAP-FGPM, 0, STD, 155, 155, 200, 150, 19, 3,                      "f(HW flow):", LEFT, -120,  5, 0, LEFT, 4, 5, "Quadratic eqn: coil capacity as a function of hot water flow rate"
         
         LABEL, "Total Capacity as f(part load)", STD,   LEFT,  20, 190, 1, 0, 0, 305, 0, 3
         COMBO, 13395, 13395, 0, 1, SYSTEM, 0,  HEAT-CLOSS-FPLR, 0, STD, 155, 215, 200, 150, 19, 3,                      "f(cycling):", LEFT, -120,  5, 0, LEFT, 4, 5, "Quadratic eqn: cycling fraction as a function of cycling part load ratio"
         COMBO, 13396, 13396, 0, 1, SYSTEM, 0,    HEAT-CAP-FRPM, 0, STD, 155, 245, 200, 150, 19, 3,                          "f(RPM):", LEFT, -120,  5, 0, LEFT, 4, 5, "Quadratic eqn: heating capacity as a function of the heat pump engine RPM"
         

         LABEL,                  "Waste Heat", STD, LEFT, 350, 10, 1, 0, 0, 655, 0, 3
         COMBO, 13397, 13397, 0, 1, SYSTEM, 0,   WASTE-HEAT-USE, 0, STD, 495,  35,  85, 160, 19, 3,                  "Waste Heat Use:", LEFT, -130,  5, 0, LEFT, 4, 5, "The end use of the waste heat that is recovered from the Gas Heat Pump"
         COMBO, 13529, 13529, 0, 1, SYSTEM, 0,  HTREC-DW-HEATER, 0, STD, 495,  65, 200, 160, 19, 3,               "Ht Rec DHW Heater:", LEFT, -130,  5, 0, LEFT, 4, 5, "Name of the DHW Heater that receives the superheat from the air conditioner"
          EDIT, 13254, 13254, 0, 1, SYSTEM, 0,   MAX-COND-RCVRY, 0, STD, 560,  95,  23,  50,  2, 3,    "Max Cond Recvry for Spc Heat:", LEFT, -195,  5, 1, LEFT, 4, 5, "Max fraction of condenser heat that can be recovered (and used to replace active heating)"

         LABEL, "Waste Heat Available from Cooling and Heating", STD, LEFT, 350, 130, 1, 0, 0, 655, 0, 3
          EDIT, 13398, 13398, 0, 1, SYSTEM, 0,  COOL-WASTE-HEAT, 0, STD, 560, 155,  23,  50,  2, 3, "Frac Heat Input Avail from Cool:", LEFT, -195,  5, 1, LEFT, 4, 5, "Fraction of heat input to gas cooling unit (or cooling load for electric) that is recoverable heat"
         COMBO, 13399, 13399, 0, 1, SYSTEM, 0,       COOL-WH-FT, 0, STD, 515, 185, 200, 140, 19, 3,           "Waste Ht Cap from Cool", LEFT, -150, -4, 0, LEFT, 4, 5, "Quadratic eqn:availability of Cooling Waste Heat as fct of entering wetbulb & outside drybulb"
         LABEL,          "f(outdoor drybulb):",  STD,   LEFT,  390, 197, 1, 0, 0, 0, 13399, 3
         COMBO, 13419, 13419, 0, 1, SYSTEM, 0,     COOL-WH-FRPM, 0, STD, 515, 215, 200, 140, 19, 3,           "Waste Ht Cap from Cool", LEFT, -150, -4, 0, LEFT, 4, 5, "Quadratic eqn: waste heat generated by engine as a function of the of the compressor RPM"
         LABEL,           "f(compressor RPM):",  STD,   LEFT,  390, 227, 1, 0, 0, 0, 13419, 3
         
;@1       LABEL, "Waste Heat Input to Heating:", STD,   LEFT, 315, 247, 1, 0, 0, 0, 0, 3
          EDIT, 13420, 13420, 0, 1, SYSTEM, 0,  HEAT-WASTE-HEAT, 0, STD, 560, 245,  23,  50,  2, 3, "Frac Heat Input Avail from Heat:", LEFT, -195,  5, 1, LEFT, 4, 5, ""
         COMBO, 13421, 13421, 0, 1, SYSTEM, 0,       HEAT-WH-FT, 0, STD, 515, 275, 200, 140, 19, 3,           "Waste Ht Cap from Heat", LEFT, -150, -4, 0, LEFT, 4, 5, "Quadratic eqn: availability of Heating Waste Heat as fct of outside drybulb temp"
         LABEL,          "f(outdoor drybulb):",  STD,   LEFT, 390, 287, 1, 0, 0, 0, 13421, 3
         COMBO, 13422, 13422, 0, 1, SYSTEM, 0,     HEAT-WH-FRPM, 0, STD, 515, 305, 200, 140, 19, 3,           "Waste Ht Cap from Heat", LEFT, -150, -4, 0, LEFT, 4, 5, "Quadratic eqn: waste heat generated by engine as a function of the of the compressor RPM"
         LABEL,           "f(compressor RPM):",  STD,   LEFT, 390, 317, 1, 0, 0, 0, 13422, 3
    

; SAC 1/16/06 - added staged volume subtab page from JJH
       SUBTABPAGE, 3364, 29047, 1, 3, " Stages "
         
        CASE, SYSTEM, 0, TYPE, -1, =, 1, 28
        ;PVVT systems
          COMBO, 17935, 13450, 0, 1, SYSTEM, 0,  AIR/TEMP-CONTROL,0, STD, 240,   5,  80, 145, 19, 3,            "Heating & Cooling Staging Control:", LEFT, -205, 5, 0, LEFT, 4, 5, ""

          LABEL,"Cooling Stages", STD, CENTER, 160,  33, 1, 0, 0, 0, 0, 3

          LABEL,     "Capacity",  STD, CENTER, 125,  49, 1, 0, 0, 0, 0, 3
          LABEL,     "Fraction",  STD, CENTER, 125,  65, 1, 0, 0, 0, 0, 3
         
          LABEL,     "Delta T",   STD, CENTER, 205,  49, 1, 0, 0, 0, 0, 3
          LABEL,     "°F",        STD, CENTER, 205,  65, 1, 0, 0, 0, 0, 3
          
          LABEL,"Heating Stages", STD, CENTER, 320,  33, 1, 0, 0, 0, 0, 3

          LABEL,     "Capacity",  STD, CENTER, 280,  49, 1, 0, 0, 0, 0, 3
          LABEL,     "Fraction",  STD, CENTER, 280,  65, 1, 0, 0, 0, 0, 3
         
          LABEL,     "Delta T",   STD, CENTER, 355,  49, 1, 0, 0, 0, 0, 3
          LABEL,     "°F",        STD, CENTER, 355,  65, 1, 0, 0, 0, 0, 3
         
          LABEL, "Stage 1:", STD, LEFT, 35,  85, 1, 0, 0, 0, 0, 3
          LABEL, "Stage 2:", STD, LEFT, 35, 110, 1, 0, 0, 0, 0, 3
          LABEL, "Stage 3:", STD, LEFT, 35, 135, 1, 0, 0, 0, 0, 3
          LABEL, "Stage 4:", STD, LEFT, 35, 160, 1, 0, 0, 0, 0, 3

          EDIT, 17936, 12306, 0, 1, SYSTEM, 0,  COOL-STAGES    , 0, STD,  90,  80,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" 
          EDIT, 17937, 13066, 0, 1, SYSTEM, 0,  COOL-STAGES    , 1, STD,  90, 105,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17938, 12307, 0, 1, SYSTEM, 0,  COOL-STAGES    , 2, STD,  90, 130,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" 
          EDIT, 17939, 12307, 0, 1, SYSTEM, 0,  COOL-STAGES    , 3, STD,  90, 155,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, "" 
          
          EDIT, 17940, 13430, 0, 1, SYSTEM, 0,  COOL-STAGES-DT , 0, STD, 175,  80,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17941, 13431, 0, 1, SYSTEM, 0,  COOL-STAGES-DT , 1, STD, 175, 105,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17942, 13432, 0, 1, SYSTEM, 0,  COOL-STAGES-DT , 2, STD, 175, 130,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17943, 13432, 0, 1, SYSTEM, 0,  COOL-STAGES-DT , 3, STD, 175, 155,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
                                                                                                         
          EDIT, 17944, 13433, 0, 1, SYSTEM, 0,  HEAT-STAGES    , 0, STD, 250,  80,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17945, 13434, 0, 1, SYSTEM, 0,  HEAT-STAGES    , 1, STD, 250, 105,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17946, 13435, 0, 1, SYSTEM, 0,  HEAT-STAGES    , 2, STD, 250, 130,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17947, 13435, 0, 1, SYSTEM, 0,  HEAT-STAGES    , 3, STD, 250, 155,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          
          EDIT, 17948, 13436, 0, 1, SYSTEM, 0,  HEAT-STAGES-DT , 0, STD, 325,  80,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17949, 13437, 0, 1, SYSTEM, 0,  HEAT-STAGES-DT , 1, STD, 325, 105,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17950, 13438, 0, 1, SYSTEM, 0,  HEAT-STAGES-DT , 2, STD, 325, 130,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
          EDIT, 17951, 13438, 0, 1, SYSTEM, 0,  HEAT-STAGES-DT , 3, STD, 325, 155,  23,  60,  4, 3,                        "", LEFT, -2, 5, 0, LEFT, 4, 5, ""
        ENDCASE 
        CASE, SYSTEM, 0, TYPE, -1, =, 31, 1,2,3,4,5,6,7,8,9,10,11,12,13,14,15,16,17,18,19,20,21,22,23,24,25,26,27,29,30,31,32
        ;everthing except PVVT
          LABEL, "Staged Volume and 2-speed parameters apply only to PVVT systems", STD, LEFT, 20,  15, 1, 0, 0, 0, 0, 3
        ENDCASE 

; DEM 10/26/16 - added new tab for VRF indoor coil
    ;*****************************************
    ; VRF Coil
    ;*****************************************
     TABPAGE, 3390, 32072, 1, 3, NOTIMP," VRF Coil "

      LABEL, "VRF Indoor Coil General Info",  BOLD,  LEFT, 20, 10, 1, 0, 0, 485, 19456, 3
          COMBO, 19456, 19456, 0, 1, SYSTEM, 0,  CONDENSING-UNIT,  0, STD, 195,  30, 300, 220, 19, 3,        "Condensing Unit:",  LEFT, -155, 5, 0, LEFT, 4, 5,"The U-name of a CONDENSING-UNIT to which the cooling/heating coil(s) in this system are connected.  Also need to set HEAT-SOURCE = CONDENSING-UNIT in Heating/Coil Cap-Control."
          COMBO, 19457, 19457, 0, 1, SYSTEM, 0,    VRF-TERM-TYPE,  0, STD, 195,  55, 300, 220, 19, 3,   "Indoor Terminal Type:",  LEFT, -155, 5, 0, LEFT, 4, 5,"Type of terminal for the VRF indoor unit.  Triggers default values for SUPPLY-KW/FLOW for the indoor unit. "
          COMBO, 19458, 19458, 0, 1, SYSTEM, 0, HEAT/COOL-CONFIG,  0, STD, 195,  80, 300, 220, 19, 3, "Heat/Cool Configuration:",  LEFT, -155, 5, 0, LEFT, 4, 5,"If both heating and cooling coils attached to a condensing-unit, whether a common coil"
          COMBO, 19459, 19459, 0, 1, SYSTEM, 0,    RFG-COIL-CTRL,  0, STD, 195, 105, 300, 220, 19, 3,      "Refg Coil Control:",  LEFT, -155, 5, 0, LEFT, 4, 5,"For condensing unit, specifies how the coil is controlled in response to the zone thermostat or discharge air controller"
      LABEL, "Rated and Design Conditions - Cooling",  BOLD,  LEFT, 20, 135, 1, 0, 0, 260, 19459, 3
           EDIT, 19464, 19464, 0, 1, SYSTEM, 0,        RATED-SST,  0, STD, 160, 155,  23,  70,  1, 3,              "Rated SST:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Rated saturated suction temperature for the coil in cooling. Corresponds to the rated coil cooling capacity."
           EDIT, 19465, 19465, 0, 1, SYSTEM, 0,      DES-MIN-SST,  0, STD, 160, 180,  23,  70,  1, 3,         "Design Min SST:",  LEFT, -120, 5, 1, LEFT, 4, 5,"The target SST at the indoor fan coil units during design sizing in cooling mode."
           EDIT, 19466, 19466, 0, 1, SYSTEM, 0,      DES-MAX-SST,  0, STD, 160, 205,  23,  70,  1, 3,         "Design Max SST:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Maximum SST at the coil during design sizing calculations for cooling.  The SST at the compressor will be decreased below the CONDENSING-UNIT:DES-TARGET-SST if needed to keep the coil SST from rising above this value."
      LABEL, "Rated and Design Conditions - Heating",  BOLD,  LEFT, 355, 135, 1, 0, 0, 650, 19466, 3
           EDIT, 19467, 19467, 0, 1, SYSTEM, 0,     HT-RATED-SDT,  0, STD, 500, 155,  23,  70,  1, 3,              "Rated SDT:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Rated saturated discharge temperature for the coil in heating.  Corresponds to the rated coil heating capacity."
           EDIT, 19468, 19468, 0, 1, SYSTEM, 0,      DES-MIN-SDT,  0, STD, 500, 180,  23,  70,  1, 3,         "Design Min SDT:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Target saturated discharge temperature (SDT) at the coil during design sizing calculations for heating."
           EDIT, 19469, 19469, 0, 1, SYSTEM, 0,      DES-MAX-SDT,  0, STD, 500, 205,  23,  70,  1, 3,         "Design Max SDT:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Minimum saturated discharge temperature (SDT) at the coil during design sizing calculations for heating.  The SDT at the compressor will be increased above the CONDENSING-UNIT:DES-TARGET-SDT if needed to keep the coil SDT from falling below this value."
      LABEL, "VRF Branch Pipe Geometry",  BOLD,  LEFT, 20, 235, 1, 0, 0, 460, 19469, 3
           EDIT, 19474, 19474, 0, 1, SYSTEM, 0,       VRF-PIPE-L,  0, STD, 170, 255,  23,  70,  1, 3,            "Pipe Length:",  LEFT, -130, 5, 1, LEFT, 4, 5,"The length of the branch refrigerant pipe."
           EDIT, 19475, 19475, 0, 1, SYSTEM, 0,    VRF-FITTING-L,  0, STD, 170, 280,  23,  70,  1, 3,      "Fitting Equiv Len:",  LEFT, -130, 5, 1, LEFT, 4, 5,"The equivalent length of fittings in the branch refrigerant pipe.  This affects pipe friction, but not thermal loss."
           EDIT, 19476, 19476, 0, 1, SYSTEM, 0,   VRF-GAS-PIPE-D,  0, STD, 170, 305,  23,  70,  1, 3,           "Gas Pipe Dia:",  LEFT, -130, 5, 1, LEFT, 4, 5,"The nominal diameter of the gas refrigerant pipe for the indoor unit.  If not entered, the program will calculate a diameter based on common practice."
          COMBO, 19477, 19477, 0, 1, SYSTEM, 0,     VRF-PIPE-LOC,  0, STD, 170, 330, 300, 220, 19, 3,          "Pipe Location:",  LEFT, -130, 5, 0, LEFT, 4, 5,"The location of the branch refrigerant pipe for calculating thermal loss.  OUTDOOR will use the hourly outdoor temperature, and ZONE will use the temperature of a specified zone."
          COMBO, 19478, 19478, 0, 1, SYSTEM, 0,    VRF-PIPE-ZONE,  0, STD, 170, 355, 300, 220, 19, 3,              "Pipe Zone:",  LEFT, -130, 5, 0, LEFT, 4, 5,"The zone in which the branch refrigerant pipe is located if VRF-PIPE-LOC = ZONE."


    ;*****************************************
    ; PreCond
    ;*****************************************
    TABPAGE, 3057, 29074, 1, 3, NOTIMP, " Preconditioner "
    
;  RADIOFIRST, 29033, 29033, 0, 1, 0, PowerDOE, 0, SysModePreCond,    0, 0, STD,  17, 14,  18, 143, 3,   "Add-On Evap Cooling", LEFT, ""
;  RADIONEXT,  29034, 29034, 0, 1, 0, PowerDOE, 0, SysModePreCond2,   0, 1, STD, 170, 14,  18, 128, 3,      "Add-On Desiccant", LEFT, ""
;  RADIONEXT,  29041, 29041, 0, 1, 0, PowerDOE, 0, SysModePreCond3,   0, 2, STD, 308, 14,  18, 120, 3,       "Pckgd Desiccant", LEFT, ""
;  RADIONEXT,  29024, 29024, 0, 1, 0, PowerDOE, 0, SysModePreCond4,   0, 3, STD, 438, 14,  18, 148, 3, "Desiccant Perf Curves", LEFT, ""

       SUBTABPAGE, 3188, 29033, 1, 3, "  Add-On Evaporative Cooling  "

;@4@  for system type = EVAP-COOLER or RESYS, Add-On Evaporative Cooling does not apply.
         CASE, SYSTEM, 0, TYPE, -1, =, 2, 17, 26
            LABEL, "Not applicable for systems:  Evaporative Cooler or Residential System", STD, CENTER, 340, 32, 1, 0, 0, 0, 0, 3
            LABEL, "See instead, the Cooling tab, Evap Cooling subtab",                     STD, CENTER, 340, 52, 1, 0, 0, 0, 0, 3
         ENDCASE     
          
;        for all system types except EVAP-COOLER or RESYS, display Add-On Evaporative Cooling controls
;        CASE, SYSTEM, 0, TYPE, -1, =, 30, 1,2,3,4,5,6,7,8,9,10,11,12,13,14,15,16,18,19,20,21,22,23,24,25,27,28,29,30,31,32
         CASE, ELSE
            LABEL, "Add-On Evaporative Cooling", STD, LEFT, 20, 30, 1, 0, 0, 645, 0, 3
            COMBO, 13307, 13458, 0, 1, SYSTEM, 0,     EVAP-CL-TYPE, 0, STD, 185,  50, 110, 135, 19, 3,                  "Evap Cooler Type:", LEFT, -150, 5, 0, LEFT, 4, 5, "Type of evaporative cooling element (Direct and/or Indirect or None)"
            COMBO, 13306, 13306, 0, 1, SYSTEM, 0,    EVAP-CL+M-SUP, 0, STD, 185,  75,  85, 135, 19, 3,             "Evap + Main Cool Coil:", LEFT, -150, 5, 0, LEFT, 4, 5, "Whether the evaporative cooler can operate in conjunction with mechanical cooling"
            COMBO, 13308, 13297, 0, 1, SYSTEM, 0,   EVAP-CL+REC-RA, 0, STD, 240, 100,  85,  80, 19, 3, "Return Air Used at Indirect Stage:", LEFT, -205, 5, 0, LEFT, 4, 5, "Whether return air is used for the secondary air-stream of the indirect evaporative cooler"
;            EDIT, 13311, 13311, 0, 1, SYSTEM, 0,        RECOV-EFF, 0, STD, 230, 275,  23,  60,  2, 3,             "Indirect Recovery Eff:", LEFT, -195, 5, 1, LEFT, 4, 5, ""
              
             EDIT, 13314, 13314, 0, 1, SYSTEM, 0,  EVAP-CL-LIMIT-T, 0, STD, 535,  50,  23,  70,  1, 3,                "Drybulb High Limit:", LEFT, -160, 5, 1, LEFT, 4, 5, "Outside air (drybulb) temperature above which the evaporative cooler is turned off"
             EDIT, 13315, 13464, 0, 1, SYSTEM, 0,      EVAP-CL-AIR, 0, STD, 535,  75,  23,  70,  2, 3,          "Evap Frac of Design Flow:", LEFT, -160, 5, 1, LEFT, 4, 5, "Fraction of design supply air that is allowed to pass through the evaporative cooler"
             EDIT, 13316, 13300, 0, 1, SYSTEM, 0,  EVAP-CL-KW/FLOW, 0, STD, 535, 100,  23,  70,  6, 3,               "Pump & Secondary kW:", LEFT, -160, 5, 1, LEFT, 4, 5, "Power consumption of evaporative cooling pump and secondary fan (per unit air flow)"

            LABEL, "Rating",       STD, CENTER, 215, 143, 1, 0, 0, 0, 13309, 3
            LABEL, "f(air flow)",  STD, CENTER, 345, 159, 1, 0, 0, 0, 13309, 3
             EDIT, 13309, 13298, 0, 1, SYSTEM, 0,       DIRECT-EFF, 0, STD, 185, 175,  23,  60,  2, 3,              "Direct Effectiveness:", LEFT, -150, 5, 1, CENTER, -30, -16, "Rated (nominal) effectiveness of the direct evaporative cooler"
            COMBO, 13313, 13313, 0, 1, SYSTEM, 0, DIRECT-EFF-FFLOW, 0, STD, 260, 175, 300, 180, 19, 3,                                   "", LEFT,   -5, 5, 0, LEFT,     4,   5, "Cubic eqn: effectiveness of direct evaporative cooling as a function of the air flow"
             EDIT, 13310, 13299, 0, 1, SYSTEM, 0,        INDIR-EFF, 0, STD, 185, 200,  23,  60,  2, 3,            "Indirect Effectiveness:", LEFT, -150, 5, 0, LEFT,     4,   5, "Rated (nominal) effectiveness of the indirect evaporative cooler"
            COMBO, 13317, 13317, 0, 1, SYSTEM, 0,  INDIR-EFF-FFLOW, 0, STD, 260, 200, 300, 180, 19, 3,                                   "", LEFT,   -5, 5, 0, LEFT,     4,   5, "Cubic eqn: effectiveness of indirect evaporative cooling as a function of the air flow"
         ENDCASE     


       SUBTABPAGE, 3189, 29034, 1, 3, "  Add-On Desiccant  "

         LABEL, "Add-On Desiccant Cooling", STD, LEFT, 20, 30, 1, 0, 0, 315, 0, 3
          COMBO, 13318, 14001, 0, 1, SYSTEM, 0,        DESICCANT, 0, STD, 170,  50, 110, 145, 19, 3,                  "Desiccant Sys Type:", LEFT, -135, 5, 0, LEFT, 4, 5, "The type of add-on (integrated) desiccant unit"
          COMBO, 13319, 14003, 0, 1, SYSTEM, 0, DESC-HEAT-SOURCE, 0, STD, 170,  75, 190, 145, 19, 3,                   "Desic Heat Source:", LEFT, -135, 5, 0, LEFT, 4, 5, "The source of heat used to regenerate (dry out) the desiccant and provide space heating"
           EDIT, 13320, 14002, 0, 1, SYSTEM, 0,    DESICCANT-AIR, 0, STD, 240, 100,  23,  60,  2, 3,           "Desic Frac of Design Flow:", LEFT, -205, 5, 1, LEFT, 4, 5, "Air flow rate through the desiccant (as a fraction of the design supply air flow rate)"
           EDIT, 13152, 13152, 0, 1, SYSTEM, 0,   DESC-CTRL-MODE, 0, STD, 240, 125,  23,  60,  0, 3,       "Desic Ctrl Mode/Configuration:", LEFT, -205, 5, 0, LEFT, 4, 5, "The control mode of the add-on (integrated) desiccant unit"
           
          COMBO, 14515, 14515, 0, 1, SYSTEM, 0,        DESC-LOOP, 0, STD, 170, 150, 200, 145, 19, 3,              "Desic Circulation Loop:", LEFT, -135, 5, 0, LEFT, 4, 5, "Name of loop that supplies heat to the desiccant unit"
          COMBO, 14516, 14516, 0, 1, SYSTEM, 0,     DESC-CHILLER, 0, STD, 170, 175, 200, 145, 19, 3,                   "Desiccant Chiller:", LEFT, -135, 5, 0, LEFT, 4, 5, "Name of Chiller/Heater that provides heat to (and cools) the desiccant"
          COMBO, 14517, 14517, 0, 1, SYSTEM, 0,  DESC-VALVE-TYPE, 0, STD, 170, 200, 100, 145, 19, 3,                "Desiccant Valve Type:", LEFT, -135, 5, 0, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
           EDIT, 14518, 14518, 0, 1, SYSTEM, 0,   DESC-COIL-HEAD, 0, STD, 240, 225,  23,  60,  2, 3,                 "Desiccant Coil Head:", LEFT, -205, 5, 1, LEFT, 4, 5, "Pressure drop of fluid through the desiccant coil at design flow"
           EDIT, 14519, 14519, 0, 1, SYSTEM, 0,     DESC-COIL-DT, 0, STD, 240, 250,  23,  60,  1, 3,              "Desiccant Coil Delta T:", LEFT, -205, 5, 1, LEFT, 4, 5, "The temperature change through the coil (at the design conditions)"
           
         LABEL, "Liquid Vent Air 1 & 2 Systems", STD, LEFT, 355, 30, 1, 0, 0, 650, 13153, 3
           EDIT, 13153, 13153, 0, 1, SYSTEM, 0,     DESC-DEW-SET, 0, STD, 540,  50,  23,  60,  1, 3,          "Desiccant Exiting Dewpoint:", LEFT, -170, 5, 1, LEFT, 4, 5, "Dewpoint temperature setpoint of air exiting the desiccant unit"
;          EDIT, 13154, 13154, 0, 1, SYSTEM, 0,    DESC-NOM-FLOW, 0, STD, 540,  75,  23,  60,  0, 3,              "Desiccant Nominal Flow:", LEFT, -170, 5, 1, LEFT, 4, 5, ""
           
         LABEL, "Solid Vent Air 1 Heat Exchanger", STD, LEFT, 355, 130, 1, 0, 0, 650, 13321, 3
           EDIT, 13321, 13321, 0, 1, SYSTEM, 0,    HEAT-EXCH-EFF, 0, STD, 540, 150,  23,  60,  2, 3,             "Heat Exch Effectiveness:", LEFT, -170, 5, 1, LEFT, 4, 5, "The effectiveness of the sensible heat exchanger"
           EDIT, 13322, 13322, 0, 1, SYSTEM, 0,   HEAT-EXCH-DELP, 0, STD, 540, 175,  23,  60,  2, 3,                   "Heat Exch Delta P:", LEFT, -170, 5, 1, LEFT, 4, 5, "Supply air pressure drop across the sensible heat exchanger"


       SUBTABPAGE, 3190, 29041, 1, 3, "  Packaged Desiccant  "

         LABEL, "Packaged Total-Gas Solid Desiccant System Performance:", STD, LEFT, 20, 20, 1, 0, 0, 0, 0, 3
      
         LABEL, "Performance at Full Load", STD, LEFT, 35, 45, 1, 0, 0, 570, 13196, 3
         COMBO, 13196, 13196, 0, 1, SYSTEM, 0,     T8-FWB1WB6, 0, STD, 370,  65, 300, 200, 19, 3,          "Exit Temperature = f(return wb & outdoor wb):", LEFT, -320, 5, 0, LEFT, 4, 5, "Bi-Quadratic eqn: supply air drybulb (before direct evap cooler) as fct of wetbulb of exh & OA"
         COMBO, 13236, 13236, 0, 1, SYSTEM, 0,    HR8-FWB1WB6, 0, STD, 370,  90, 300, 200, 19, 3,          "Exit Humid Ratio = f(return wb & outdoor wb):", LEFT, -320, 5, 0, LEFT, 4, 5, "Bi-Quadratic eqn: ln(1000*Humidity Ratio of supply air) as fct of exh & OA wetbulb"
         COMBO, 13244, 13244, 0, 1, SYSTEM, 0,   QREG-FWB1WB6, 0, STD, 370, 115, 300, 200, 19, 3,              "Regen Energy = f(return wb & outdoor wb):", LEFT, -320, 5, 0, LEFT, 4, 5, "Bi-Quadratic eqn: regeneration energy as function of exhaust & OA wetbulb temps"
      
         LABEL, "Performance at 25% Part Load", STD, LEFT, 35, 155, 1, 0, 0, 570, 13312, 3
         COMBO, 13312, 13312, 0, 1, SYSTEM, 0,   T8PL-FWB1WB6, 0, STD, 370, 175, 300, 200, 19, 3,  "Exit Temperature, 25% pl = f(return wb & outdoor wb):", LEFT, -320, 5, 0, LEFT, 4, 5, "Bi-Quadratic eqn: ln(1000*supply air Humidity Ratio) as fct of exh & OA wetbulb @ 25% PLR"
         COMBO, 13323, 13323, 0, 1, SYSTEM, 0,  HR8PL-FWB1WB6, 0, STD, 370, 200, 300, 200, 19, 3,  "Exit Humid Ratio, 25% pl = f(return wb & outdoor wb):", LEFT, -320, 5, 0, LEFT, 4, 5, "Bi-Quadratic eqn: ln(1000*supply air Humidity Ratio) as fct of exh & OA wetbulb at 25% PLR"
         COMBO, 13324, 13324, 0, 1, SYSTEM, 0, QREGPL-FWB1WB6, 0, STD, 370, 225, 300, 200, 19, 3,      "Regen Energy, 25% pl = f(return wb & outdoor wb):", LEFT, -320, 5, 0, LEFT, 4, 5, "Bi-Quadratic eqn: regeneration energy as a fct of exhaust & OA wetbulb at 25% PLR"


       SUBTABPAGE, 3191, 29024, 1, 3, "  Desiccant Performance Curves  "

         LABEL, "System Performance (Liq Vent Air 1 only)", STD, LEFT, 35, 45, 1, 0, 0, 540, 13148, 3
          COMBO, 13148, 13148, 0, 1, SYSTEM, 0,    DESC-T-FTW, 0, STD, 340,  65, 300, 200, 19, 3,        "Exit Temperature = f(entering t & humid ratio):", LEFT, -290, 5, 0, LEFT, 4, 5, ""
          COMBO, 13149, 13149, 0, 1, SYSTEM, 0,    DESC-W-FTW, 0, STD, 340,  90, 300, 200, 19, 3,     "Exit Humidity Ratio = f(entering t & humid ratio):", LEFT, -290, 5, 0, LEFT, 4, 5, ""
          COMBO, 13150, 13150, 0, 1, SYSTEM, 0,  DESC-GAS-FTW, 0, STD, 340, 115, 300, 200, 19, 3,               "Gas Usage = f(entering t & humid ratio):", LEFT, -290, 5, 0, LEFT, 4, 5, ""
          COMBO, 13151, 13151, 0, 1, SYSTEM, 0,   DESC-KW-FTW, 0, STD, 340, 140, 300, 200, 19, 3,            "Auxiliary kW = f(entering t & humid ratio):", LEFT, -290, 5, 0, LEFT, 4, 5, ""
        
    
    ;*****************************************
    ; Meters 
    ;*****************************************
    TABPAGE, 3058, 29053, 1, 3, NOTIMP, "  Meters  "

      LABEL, "System-Level Meter Assignments by End-Use:", STD, LEFT, 30, 15, 1, 0, 0, 0, 0, 3
      
      LABEL, "Electric Meters", STD, LEFT, 55, 40, 1, 0, 0, 575, 0, 3
      COMBO, 13325, 12205, 32079, 1, SYSTEM, 0,  MSTR-ELEC-METER, 0, STD, 190,  60, 300, 100, 19, 3,  "Master Elec Meter:", LEFT, -120, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies all of the unassigned system electric consumption"
      COMBO, 13326, 12865, 32079, 1, SYSTEM, 0, LIGHT-ELEC-METER, 0, STD, 190,  85, 300, 100, 19, 3,      "Area Lighting:", LEFT, -120, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the system's Area Lighting electric consumption"
      COMBO, 13327, 12925, 32079, 1, SYSTEM, 0,  TASK-ELEC-METER, 0, STD, 190, 110, 300, 100, 19, 3,      "Task Lighting:", LEFT, -120, 5, 0, LEFT, 4, 5, "Electric Meter that tallies the system's Task Lighting electricity consumption"
      COMBO, 13328, 12926, 32079, 1, SYSTEM, 0, EQUIP-ELEC-METER, 0, STD, 190, 135, 300, 100, 19, 3,     "Elec Equipment:", LEFT, -120, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the system's Equipment electricity consumption"
      COMBO, 13329, 13329, 32079, 1, SYSTEM, 0, SOURCE-ELEC-METE, 0, STD, 190, 160, 300, 100, 19, 3,        "Source Elec:", LEFT, -120, 5, 0, LEFT, 4, 5, ""
      COMBO, 13330, 13545, 32079, 1, SYSTEM, 0,  HEAT-ELEC-METER, 0, STD, 190, 185, 300, 100, 19, 3,      "Space Heating:", LEFT, -120, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the system's Space Heating electricity consumption"
      COMBO, 13331, 13585, 32079, 1, SYSTEM, 0,  COOL-ELEC-METER, 0, STD, 190, 210, 300, 100, 19, 3,      "Space Cooling:", LEFT, -120, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the system's Space Cooling electric consumption"

      COMBO, 13332, 13332, 32079, 1, SYSTEM, 0, HTREJ-ELEC-METER, 0, STD, 475,  60, 300, 100, 19, 3,     "Heat Rejection:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the electric energy required for the system's heat rejection"
      COMBO, 13333, 13333, 32079, 1, SYSTEM, 0,   AUX-ELEC-METER, 0, STD, 475,  85, 300, 100, 19, 3,     "Pumps and Misc:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the system's auxiliary electric energy (e.g., pumps)"
      COMBO, 13334, 13586, 32079, 1, SYSTEM, 0,  VENT-ELEC-METER, 0, STD, 475, 110, 300, 100, 19, 3,   "Ventilation Fans:", LEFT, -130, 5, 0, LEFT, 4, 5, "Electric Meter that tallies the system Ventilation Fans electricity consumption"
      COMBO, 13335, 13335, 32079, 1, SYSTEM, 0,  REFG-ELEC-METER, 0, STD, 475, 135, 300, 100, 19, 3,      "Refrigeration:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's refrigeration electric energy consumption"
      COMBO, 13336, 13587, 32079, 1, SYSTEM, 0,  SUPP-ELEC-METER, 0, STD, 475, 160, 300, 100, 19, 3,  "Supplemental Heat:", LEFT, -130, 5, 0, LEFT, 4, 5, "Electric Meter that tallies the system's electric consumption for supplemental heating"
      COMBO, 13337, 13588, 32079, 1, SYSTEM, 0,   DHW-ELEC-METER, 0, STD, 475, 185, 300, 100, 19, 3, "Domestic Hot Water:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the system's DHW heater electricity consumption"

      LABEL, "Fuel Meters", STD, LEFT, 55, 250, 1, 0, 0, 575, 0, 3
      COMBO, 13338, 13589, 32079, 1, SYSTEM, 0,  MSTR-FUEL-METER, 0, STD, 190, 270, 300, 100, 19, 3,  "Master Fuel Meter:", LEFT, -120, 5, 0, LEFT, 4, 5, "Name of Fuel Meter that tallies all of the unassigned system fuel consumption"
      COMBO, 13339, 13339, 32079, 1, SYSTEM, 0, SOURCE-FUEL-METE, 0, STD, 190, 295, 300, 100, 19, 3,        "Source Fuel:", LEFT, -120, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the zone's 'source' fuel consumption"
      COMBO, 13340, 13590, 32079, 1, SYSTEM, 0,  HEAT-FUEL-METER, 0, STD, 190, 320, 300, 100, 19, 3,      "Space Heating:", LEFT, -120, 5, 0, LEFT, 4, 5, "Name of Fuel Meter that tallies all of the unassigned system fuel consumption"

      COMBO, 13341, 13591, 32079, 1, SYSTEM, 0,  COOL-FUEL-METER, 0, STD, 475, 270, 300, 100, 19, 3,      "Space Cooling:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of the Fuel Meter that tallies the fuel consumption of this system's cooling system"
      COMBO, 13342, 13592, 32079, 1, SYSTEM, 0,  SUPP-FUEL-METER, 0, STD, 475, 295, 300, 100, 19, 3,  "Supplemental Heat:", LEFT, -130, 5, 0, LEFT, 4, 5, "Electric Meter that tallies the system's fuel consumption for supplemental heating"
      COMBO, 13372, 13593, 32079, 1, SYSTEM, 0,   DHW-FUEL-METER, 0, STD, 475, 320, 300, 100, 19, 3, "Domestic Hot Water:", LEFT, -130, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the system's DHW heater fuel consumption"

   
; SAC 11/23/10 - removed          
;    ;*****************************************
;    ; Refrig 
;    ;*****************************************
;    TABPAGE, 3059, 10261, 1, 3, NOTIMP, " Refrigeration "
;
;;  RADIOFIRST, 29010, 29010, 0, 1, 0, PowerDOE, 0, SysModeRefg,    0, 0, STD,  23, 14,  18, 110, 3,   "Design Params", LEFT, ""
;;  RADIONEXT,  29013, 29054, 0, 1, 0, PowerDOE, 0, SysModeRefg2,   0, 1, STD, 143, 14,  18, 100, 3,       "Condenser", LEFT, ""
;;  RADIONEXT,  29079, 29054, 0, 1, 0, PowerDOE, 0, SysModeRefg3,   0, 2, STD, 243, 14,  18, 115, 3,      "Heat Recov", LEFT, ""
;;  RADIONEXT,  29080, 29080, 0, 1, 0, PowerDOE, 0, SysModeRefg4,   0, 3, STD, 368, 14,  18, 115, 3,      "Anti-Sweat", LEFT, ""
;;  RADIONEXT,  29040, 62000, 0, 1, 0, PowerDOE, 0, SysModeRefg5,   0, 4, STD, 488, 14,  18,  95, 3,     "Perf Curves", LEFT, ""
;
;       SUBTABPAGE, 3192, 29010, 1, 3, "    Design Parameters    "
;
;         LABEL, "System Design Parameters (by evaporator temperature range)", STD, LEFT, 30, 40, 1, 0, 0, 515, 0, 3
;          
;         LABEL, "Refrigeration", STD, CENTER, 315, 58, 1, 0, 0, 0, 13350, 3
;         LABEL,  "Circuit Type", STD, CENTER, 315, 74, 1, 0, 0, 0, 13350, 3
;          
;         LABEL,      "Capacity", STD, CENTER, 410, 58, 1, 0, 0, 0, 13344, 3
;;        LABEL,        "Btu/hr", STD, CENTER, 410, 74, 1, 0, 0, 0, 13344, 3
;          
;         LABEL,           "EER", STD, CENTER, 485, 58, 1, 0, 0, 0, 13347, 3
;;        LABEL,         "Btu/W", STD, CENTER, 485, 74, 1, 0, 0, 0, 13347, 3
;          
;         COMBO, 13350, 13601, 751, 1, SYSTEM, 0,  REFG-COMP-GROUP, 0, STD, 270,  90,  85,  95, 19, 3, "Evaporator Temp Range 1 (coldest):", LEFT, -225, 5, 0, LEFT,     4,   5, "Whether the compressors are multiplexed or serve separate refrigeration circuits"
;         COMBO, 13351, 13602, 751, 1, SYSTEM, 0,  REFG-COMP-GROUP, 1, STD, 270, 115,  85,  95, 19, 3,           "Evaporator Temp Range 2:", LEFT, -225, 5, 0, LEFT,     4,   5, "Whether the compressors are multiplexed or serve separate refrigeration circuits"
;         COMBO, 13352, 13603, 751, 1, SYSTEM, 0,  REFG-COMP-GROUP, 2, STD, 270, 140,  85,  95, 19, 3, "Evaporator Temp Range 3 (warmest):", LEFT, -225, 5, 0, LEFT,     4,   5, "Whether the compressors are multiplexed or serve separate refrigeration circuits"
;          
;          EDIT, 13344, 13595, 751, 1, SYSTEM, 0,    REFG-COMP-CAP, 0, STD, 380,  90,  23,  60,  0, 3,                                   "", LEFT,   -2, 5, 1, CENTER, -30, -16, "The installed compressor capacity at the first (coldest) operating temperature"
;          EDIT, 13345, 13596, 751, 1, SYSTEM, 0,    REFG-COMP-CAP, 1, STD, 380, 115,  23,  60,  0, 3,                                   "", LEFT,   -2, 5, 0, LEFT,     4,   5, "The installed compressor capacity at the second (mid-level) operating temperature"
;          EDIT, 13346, 13597, 751, 1, SYSTEM, 0,    REFG-COMP-CAP, 2, STD, 380, 140,  23,  60,  0, 3,                                   "", LEFT,   -2, 5, 0, LEFT,     4,   5, "The installed compressor capacity at the third (warmest) operating temperature"
;          
;          EDIT, 13347, 13598, 751, 1, SYSTEM, 0,    REFG-COMP-EER, 0, STD, 455,  90,  23,  60,  3, 3,                                   "", LEFT,   -2, 5, 1, CENTER, -30, -16, "The efficiency of the compressor unit at the first (coldest) temperature level"
;          EDIT, 13348, 13599, 751, 1, SYSTEM, 0,    REFG-COMP-EER, 1, STD, 455, 115,  23,  60,  3, 3,                                   "", LEFT,   -2, 5, 0, LEFT,     4,   5, "The efficiency of the compressor unit at the second (mid-level) temperature level"
;          EDIT, 13349, 13600, 751, 1, SYSTEM, 0,    REFG-COMP-EER, 2, STD, 455, 140,  23,  60,  3, 3,                                   "", LEFT,   -2, 5, 0, LEFT,     4,   5, "The efficiency of the compressor unit at the third (warmest) temperature level"
;          
;          EDIT, 13343, 13594, 751, 1, SYSTEM, 0,  REFG-SIZING-RAT, 0, STD, 195, 190,  23,  60,  2, 3,           "Compressor Sizing Ratio:", LEFT, -150, 5, 1, LEFT,     4,   5, "Used to adjust the capacity of all compressors in the system"
;          EDIT, 14178, 14178, 751, 1, SYSTEM, 0, REFG-DIRECT-FRAC, 0, STD, 195, 215,  23,  60,  2, 3,            "Direct Return Fraction:", LEFT, -150, 5, 1, LEFT,     4,   5, "The fraction of case-to-space load that goes directly back to the return air plenum"
;
;         LABEL, "Walkin Box", STD, LEFT, 370, 195, 1, 0, 0, 640, 14602, 3
;          EDIT, 14602, 14602, 751, 1, SYSTEM, 0, REFG-WALKIN-LOAD, 0, STD, 455, 215,  23,  80,  2, 3,                              "Load:", LEFT,  -70, 5, 1, LEFT,     4,   5, ""
;         COMBO, 14603, 14603, 751, 1, SYSTEM, 0,  REFG-WALKIN-LOC, 0, STD, 455, 240, 200, 185, 19, 3,                          "Location:", LEFT,  -70, 5, 0, LEFT,     4,   5, ""
;         COMBO, 14604, 14604, 751, 1, SYSTEM, 0,  REFG-WALKIN-SCH, 0, STD, 455, 265, 300, 185, 19, 3,                          "Schedule:", LEFT,  -70, 5, 0, LEFT,     4,   5, ""


; SAC 11/23/10 - removed          
;       SUBTABPAGE, 3193, 29054, 1, 3, "    Condenser    "
;
;         COMBO, 13356, 13356, 751, 1, SYSTEM, 0,   REFG-COND-TYPE, 0, STD, 155, 15, 120, 130, 19, 3,                      "Condenser Type:", LEFT, -125, 5, 0, LEFT, 4, 5, "The type of condenser serving the refrigerated casework"
;         COMBO, 14601, 14601, 751, 1, SYSTEM, 0,   REFG-COND-CTRL, 0, STD, 155, 40, 120, 130, 19, 3,                   "Condenser Control:", LEFT, -125, 5, 0, LEFT, 4, 5, "The refrigeration condenser capacity control method"
;; Commented out as per Marlin 11/16        
;;        COMBO, 14199, 14199, 751, 1, SYSTEM, 0, *REFG-COND-GROUP, 0, STD, 170, ??,  85,  80, 19, 3,                  "Condenser Grouping:", LEFT, -150, 5, 0, LEFT, 4, 5, ""
;         
;;        LABEL,         "evaporator", STD, LEFT,    18, 107, 1, 0, 0, 0, 0, 3
;;        LABEL, "temperature range:", STD, LEFT,    18, 121, 1, 0, 0, 0, 0, 3
;;        LABEL,          "Cond Size", STD, CENTER, 180, 114, 1, 0, 0, 0, 0, 3
;;        LABEL,                "Btu", STD, CENTER, 180, 128, 1, 0, 0, 0, 0, 3
;         LABEL, "Condenser Size:",                   STD, LEFT, 31,  82, 1, 0, 0, 0, 14200, 3
;         LABEL, "(by evaporator temperature range)", STD, LEFT, 50,  98, 1, 0, 0, 0, 14200, 3
;
;          EDIT, 14200, 14202, 751, 1, SYSTEM, 0,    REFG-COND-SIZE, 0, STD, 155, 115,  23,  80,  0, 3,                           "coldest:", LEFT,  -65, 5, 1, LEFT, 4, 5, "The capacities of the condensers; definition & units depends on the Condenser Type"
;          EDIT, 14201, 14202, 751, 1, SYSTEM, 0,    REFG-COND-SIZE, 1, STD, 155, 140,  23,  80,  0, 3,                               "med:", LEFT,  -65, 5, 1, LEFT, 4, 5, "The capacities of the condensers; definition & units depends on the Condenser Type"
;          EDIT, 14202, 14202, 751, 1, SYSTEM, 0,    REFG-COND-SIZE, 2, STD, 155, 165,  23,  80,  0, 3,                           "warmest:", LEFT,  -65, 5, 1, LEFT, 4, 5, "The capacities of the condensers; definition & units depends on the Condenser Type"
;         
;;        LABEL,          "Fan Pwr", STD, CENTER, 260, 114, 1, 0, 0, 0, 0, 3
;;        LABEL,             "Frac", STD, CENTER, 260, 128, 1, 0, 0, 0, 0, 3
;; Commented out as per Marlin 11/16        
;;         EDIT, 14203, 14205, 751, 1, SYSTEM, 0,   *REFG-FAN-FRAC, 0, STD, 235, 147,  23,  50,  0, 3,                                    "", LEFT, -215, 5, 0, LEFT, 4, 5, ""
;; Commented out as per Marlin 11/16        
;;         EDIT, 14204, 14205, 751, 1, SYSTEM, 0,   *REFG-FAN-FRAC, 1, STD, 235, 172,  23,  50,  0, 3,                                    "", LEFT, -215, 5, 0, LEFT, 4, 5, ""
;; Commented out as per Marlin 11/16        
;;         EDIT, 14205, 14205, 751, 1, SYSTEM, 0,   *REFG-FAN-FRAC, 2, STD, 235, 197,  23,  50,  0, 3,                                    "", LEFT, -215, 5, 0, LEFT, 4, 5, ""
;      
;         CASE, SYSTEM, 0, REFG-COND-TYPE, -1, =, 1, 1
;            LABEL, "Air/Evap Condenser Parameters", STD, LEFT, 355, 20, 1, 0, 0, 635, 0, 3
;            COMBO, 14210, 14210, 751, 1, SYSTEM, 0,  REFG-SETPT-CTRL, 0, STD, 545,  40,  85,  90, 19, 3,                   "Setpoint Control:", LEFT, -175, 5, 0, LEFT, 4, 5, "The method used to control the refrigerators' condensers"
;               CASE, SYSTEM, 0, REFG-SETPT-CTRL, -1, =, 1, 0
;                   EDIT, 14211, 14211, 751, 1, SYSTEM, 0,   REFG-SETPT-VAL, 0, STD, 545,  65,  23,  60,  1, 3,         "Condenser Setpoint T:", LEFT, -175, 5, 1, LEFT, 4, 5, "The condenser setpoint temperature"
;               ENDCASE
;               CASE, SYSTEM, 0, REFG-SETPT-CTRL, -1, =, 1, 1
;                   EDIT, 14219, 14211, 751, 1, SYSTEM, 0,   REFG-SETPT-VAL, 0, STD, 545,  65,  23,  60,  1, 3,   "Condenser Setpoint Delta T:", LEFT, -175, 5, 1, LEFT, 4, 5, "The condenser setpoint temperature"
;               ENDCASE
;             EDIT, 14212, 14212, 751, 1, SYSTEM, 0,  REFG-MIN-COND-T, 0, STD, 545,  90,  23,  60,  1, 3,            "Minimum Condensing Temp:", LEFT, -175, 5, 1, LEFT, 4, 5, "OA thermostat setpoint:modulates condenser (or cooling tower) to maintain condensing temp"
;             EDIT, 14213, 14213, 751, 1, SYSTEM, 0,      REFG-FAN-KW, 0, STD, 545, 115,  23,  60,  1, 3,                "Condenser Fan Power:", LEFT, -175, 5, 1, LEFT, 4, 5, "Power consumption of fans of air cooled condensers or cooling towers"
;         ENDCASE 
;          
;         CASE, SYSTEM, 0, REFG-COND-TYPE, -1, =, 1, 2
;            LABEL, "Air/Evap Condenser Parameters", STD, LEFT, 355, 20, 1, 0, 0, 635, 0, 3
;            COMBO, 14215, 14210, 751, 1, SYSTEM, 0,  REFG-SETPT-CTRL, 0, STD, 545,  40,  85,  90, 19, 3,                   "Setpoint Control:", LEFT, -175, 5, 0, LEFT, 4, 5, "The method used to control the refrigerators' condensers"
;               CASE, SYSTEM, 0, REFG-SETPT-CTRL, -1, =, 1, 0
;                   EDIT, 14216, 14211, 751, 1, SYSTEM, 0,   REFG-SETPT-VAL, 0, STD, 545,  65,  23,  60,  1, 3,         "Condenser Setpoint T:", LEFT, -175, 5, 1, LEFT, 4, 5, "The condenser setpoint temperature"
;               ENDCASE
;               CASE, SYSTEM, 0, REFG-SETPT-CTRL, -1, =, 1, 1
;                   EDIT, 14220, 14211, 751, 1, SYSTEM, 0,   REFG-SETPT-VAL, 0, STD, 545,  65,  23,  60,  1, 3,   "Condenser Setpoint Delta T:", LEFT, -175, 5, 1, LEFT, 4, 5, "The condenser setpoint temperature"
;               ENDCASE
;             EDIT, 14217, 14212, 751, 1, SYSTEM, 0,  REFG-MIN-COND-T, 0, STD, 545,  90,  23,  60,  1, 3,            "Minimum Condensing Temp:", LEFT, -175, 5, 1, LEFT, 4, 5, "OA thermostat setpoint:modulates condenser (or cooling tower) to maintain condensing temp"
;             EDIT, 14218, 14213, 751, 1, SYSTEM, 0,      REFG-FAN-KW, 0, STD, 545, 115,  23,  60,  1, 3,                "Condenser Fan Power:", LEFT, -175, 5, 1, LEFT, 4, 5, "Power consumption of fans of air cooled condensers or cooling towers"
;             EDIT, 14214, 14214, 751, 1, SYSTEM, 0,     REFG-PUMP-KW, 0, STD, 545, 140,  23,  60,  1, 3,               "Condenser Pump Power:", LEFT, -175, 5, 1, LEFT, 4, 5, "Total power consumption of cooling tower condenser water pumps"
;         ENDCASE 
;          
;         CASE, SYSTEM, 0, REFG-COND-TYPE, -1, =, 1, 3
;            LABEL, "Water-Cooled Condenser Parameters", STD, LEFT, 355, 195, 1, 0, 0, 640, 0, 3
;            COMBO, 19102, 19102, 751, 1, SYSTEM, 0,     REFG-CW-LOOP, 0, STD, 480, 215,  85, 160, 19, 3,                     "Refrig CW Loop:", LEFT, -110, 5, 1, LEFT, 4, 5, "Name of loop that removes condenser heat (must be Condenser Water)"
;            COMBO, 14207, 14207, 751, 1, SYSTEM, 0,    REFG-CW-VALVE, 0, STD, 540, 240,  85, 100, 19, 3,                    "Refrig CW Valve:", LEFT, -170, 5, 1, LEFT, 4, 5, "2Way - flow varies with load; 3Way - bypasses extra fluid to maintain constant loop flowrate"
;             EDIT, 14208, 14208, 751, 1, SYSTEM, 0,     REFG-CW-HEAD, 0, STD, 575, 265,  23,  50,  1, 3,                     "Refrig CW Head:", LEFT, -205, 5, 1, LEFT, 4, 5, "Pressure drop of fluid through the refrigerant condenser"
;             EDIT, 14209, 14209, 751, 1, SYSTEM, 0,       REFG-CW-DT, 0, STD, 575, 290,  23,  50,  1, 3,                  "Refrig CW Delta T:", LEFT, -205, 5, 1, LEFT, 4, 5, "Temperature change through the condenser at the design conditions"
;         ENDCASE 


; SAC 11/23/10 - removed          
;       SUBTABPAGE, 3194, 29054, 1, 3, "    Heat Recovery    "
;
;         LABEL, "Compressors Available for Heat Recovery:", STD, LEFT, 30, 27, 1, 0, 0, 0, 13353, 3
;         LABEL,        "(by evaporator temperature range)", STD, LEFT, 60, 43, 1, 0, 0, 0, 13353, 3
;         COMBO, 13353, 13604, 751, 1, SYSTEM, 0, REFG-HTREC-UNITS, 0, STD,  90,  75,  85,  80, 19, 3,                              "coldest", CENTER,  35, -16, 0, LEFT, 4, 5, "Whether compressor that serves the first (coldest) evaporator temp allows heat recovery"
;         COMBO, 13354, 13605, 751, 1, SYSTEM, 0, REFG-HTREC-UNITS, 1, STD, 185,  75,  85,  80, 19, 3,                                  "med", CENTER,  35, -16, 0, LEFT, 4, 5, "Whether compressor that serves the second (mid-level) evaporator temp allows heat recovery"
;         COMBO, 13355, 13606, 751, 1, SYSTEM, 0, REFG-HTREC-UNITS, 2, STD, 280,  75,  85,  80, 19, 3,                              "warmest", CENTER,  35, -16, 0, LEFT, 4, 5, "Whether compressor that serves the third (warmest) evaporator temp allows heat recovery"
;   
;         COMBO, 13361, 13361, 751, 1, SYSTEM, 0, REFG-HTREC-GROUP, 0, STD, 210, 150,  85,  80, 19, 3,              "Heat Recovery Grouping:", LEFT, -180, 5, 0, LEFT, 4, 5, "Governs how many condensers heat can be recovered from when a space heating load exists"
;          EDIT, 13362, 13362, 751, 1, SYSTEM, 0,   REFG-MAX-HTREC, 0, STD, 210, 175,  23,  80,  0, 3,              "Total Recoverable Heat:", LEFT, -180, 5, 1, LEFT, 4, 5, "Maximum amount of compressor heat that is recoverable"
;          EDIT, 13363, 13363, 751, 1, SYSTEM, 0,     REFG-HTREC-T, 0, STD, 230, 200,  23,  60,  1, 3,         "Heat Recovery Cond Setpoint:", LEFT, -200, 5, 1, LEFT, 4, 5, "Condensing setpoint temperature during the heat recovery mode"
;          EDIT, 14179, 14179, 751, 1, SYSTEM, 0, REFG-HREC-STAGE1, 0, STD, 230, 225,  23,  60,  2, 3,      "Frac of Heat Recov (1st Stage):", LEFT, -200, 5, 1, LEFT, 4, 5, "Fraction of total recoverable heat from compressors in normal mode (1st stage of heat rec)"
;          EDIT, 14180, 14180, 751, 1, SYSTEM, 0, REFG-HREC-STAGE2, 0, STD, 230, 250,  23,  60,  2, 3,      "Frac of Heat Recov (2nd Stage):", LEFT, -200, 5, 1, LEFT, 4, 5, "Fraction of total recoverable heat from compressors in holdback mode (2nd stage of heat rec)"


; SAC 11/23/10 - removed          
;       SUBTABPAGE, 3195, 29080, 1, 3, "    Anti-Sweat    "
;
;;        LABEL,           "Anti-sweat Parameters:", STD, LEFT, 18, 54, 1, 0, 0, 0, 0, 3
;
;         LABEL,   "Anti-Sweat Heater Installed kW:", STD, LEFT, 30,  43, 1, 0, 0, 0, 14193, 3
;         LABEL, "(by evaporator temperature range)", STD, LEFT, 60,  59, 1, 0, 0, 0, 14193, 3
;          EDIT, 14193, 29080, 751, 1, SYSTEM, 0,    REFG-ASH-KW, 0, STD, 155,  75,  23,  60,  0, 3,                 "coldest:", LEFT,  -65, 5, 1, LEFT, 4, 5, ""
;          EDIT, 14194, 29080, 751, 1, SYSTEM, 0,    REFG-ASH-KW, 1, STD, 155, 100,  23,  60,  0, 3,                     "med:", LEFT,  -65, 5, 1, LEFT, 4, 5, "Rated power consumption of the anti-sweat heaters at second (mid-level) operating temp"
;          EDIT, 14195, 29080, 751, 1, SYSTEM, 0,    REFG-ASH-KW, 2, STD, 155, 125,  23,  60,  0, 3,                 "warmest:", LEFT,  -65, 5, 1, LEFT, 4, 5, "Rated power consumption of the anti-sweat heaters at third (warmest) operating temperature"
;          
;         LABEL, "Anti-Sweat Control Points", STD, LEFT, 365, 55, 1, 0, 0, 615, 14196, 3
;          EDIT, 14196, 14196, 751, 1, SYSTEM, 0,  REFG-ASH-LOWW, 0, STD, 530,  75,  23,  60,  2, 3,   "Absolute Humidity Low:", LEFT, -150, 5, 1, LEFT, 4, 5, "Absolute humidity of return air temperature at which the anti-sweat heaters begin to operate"
;          EDIT, 14197, 14197, 751, 1, SYSTEM, 0, REFG-ASH-HIGHW, 0, STD, 530, 100,  23,  60,  2, 3,  "Absolute Humidity High:", LEFT, -150, 5, 1, LEFT, 4, 5, "Absolute humidity of return air temp at which the anti-sweat heaters operate at full capacity"
;          
;          EDIT, 14198, 14198, 751, 1, SYSTEM, 0,  REFG-AUX-FRAC, 0, STD, 415, 200,  23,  60,  2, 3, "Fraction of Anti-Sweat and Aux Load to Refrig Case Compressors:", LEFT, -385, 5, 1, LEFT, 4, 5, "Fraction of anti-sweat heater & Auxiliary power that is a load on casework compressors"


; SAC 11/23/10 - removed          
;       SUBTABPAGE, 3196, 62000, 1, 3, "    Performance Curves    "
;
;         LABEL, "Performance Curves (by evaporator temperature range)", STD, LEFT, 30, 27, 1, 0, 0, 635, 0, 3
;      
;         LABEL,         "Compressor kW =", STD, CENTER, 195,  46, 1, 0, 0, 0, 13364, 3
;         LABEL,      "f(condensing temp)", STD, CENTER, 195,  63, 1, 0, 0, 0, 13364, 3
;          
;         LABEL,         "Compressor kW =", STD, CENTER, 375,  46, 1, 0, 0, 0, 13367, 3
;         LABEL, "f(compressor part load)", STD, CENTER, 375,  63, 1, 0, 0, 0, 13367, 3
;      
;         COMBO, 13364, 13364, 751, 1, SYSTEM, 0, REFG-KW-FTCOND, 0, STD, 115,  80, 300, 160, 19, 3,  "coldest:", LEFT,  -70, 5, 0, LEFT, 4, 5, "Cubic eqn: refrigerator power consumption as a function of the condensing temperature"
;         COMBO, 13365, 13365, 751, 1, SYSTEM, 0, REFG-KW-FTCOND, 1, STD, 115, 105, 300, 160, 19, 3,      "med:", LEFT,  -70, 5, 0, LEFT, 4, 5, "Cubic eqn: refrigerator power consumption as a function of the condensing temperature"
;         COMBO, 13366, 13366, 751, 1, SYSTEM, 0, REFG-KW-FTCOND, 2, STD, 115, 130, 300, 160, 19, 3,  "warmest:", LEFT,  -70, 5, 0, LEFT, 4, 5, "Cubic eqn: refrigerator power consumption as a function of the condensing temperature"
;      
;         COMBO, 13367, 13367, 751, 1, SYSTEM, 0,   REFG-KW-FPLR, 0, STD, 295,  80, 300, 160, 19, 3,          "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic eqn: refrigerator power consumption as a function of compressor part load ratio"
;         COMBO, 13368, 13368, 751, 1, SYSTEM, 0,   REFG-KW-FPLR, 1, STD, 295, 105, 300, 160, 19, 3,          "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic eqn: refrigerator power consumption as a function of compressor part load ratio"
;         COMBO, 13369, 13369, 751, 1, SYSTEM, 0,   REFG-KW-FPLR, 2, STD, 295, 130, 300, 160, 19, 3,          "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic eqn: refrigerator power consumption as a function of compressor part load ratio"
;      
;         CASE, SYSTEM, 0, REFG-COND-TYPE, -1, =, 1, 1
;            LABEL, "Other Performance Curves", STD, LEFT, 30, 185, 1, 0, 0, 555, 0, 3
;            COMBO, 13370, 14186, 751, 1, SYSTEM, 0,  REFG-FAN-PWR-FPL, 0, STD, 330, 205, 300, 225, 19, 3,             "Condenser Fan kW = f(partload):", LEFT, -285, 5, 0, LEFT, 4, 5, "Cubic eqn: power consumption of condenser fan as a function of condenser part load ratio"
;            COMBO, 13371, 14185, 751, 1, SYSTEM, 0,  REFG-AMB-COND-FT, 0, STD, 330, 230, 300, 225, 19, 3,    "Condenser Cap = f(ambient drybulb temp):", LEFT, -285, 5, 0, LEFT, 4, 5, "Cubic eqn: fraction of condenser that is active as a fct of ambient temperature"
;            
;            CASE, SYSTEM, 0, REFG-HREC-STAGE2, -1, >, 1, 0
;               LABEL,      "Comp kW @stg2 HR =", STD, CENTER, 555,  46, 1, 0, 0, 0, 14181, 3
;               LABEL,      "f(condensing temp)", STD, CENTER, 555,  63, 1, 0, 0, 0, 14181, 3
;               COMBO, 14181, 14181, 751, 1, SYSTEM, 0, REFG-KW-HR-FTC, 0, STD, 475,  80, 300, 160, 19, 3,           "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic equation: compressor power as function of condensing temperature"
;               COMBO, 14182, 14181, 751, 1, SYSTEM, 0, REFG-KW-HR-FTC, 1, STD, 475, 105, 300, 160, 19, 3,           "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic equation: compressor power as function of condensing temperature"
;               COMBO, 14183, 14181, 751, 1, SYSTEM, 0, REFG-KW-HR-FTC, 2, STD, 475, 130, 300, 160, 19, 3,           "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic equation: compressor power as function of condensing temperature"
;            ENDCASE   
;         ENDCASE   
;      
;         CASE, SYSTEM, 0, REFG-COND-TYPE, -1, =, 1, 2
;            LABEL, "Other Performance Curves", STD, LEFT, 30, 185, 1, 0, 0, 555, 0, 3
;            COMBO, 14186, 14186, 751, 1, SYSTEM, 0,  REFG-FAN-PWR-FPL, 0, STD, 330, 205, 300, 225, 19, 3,             "Condenser Fan kW = f(partload):", LEFT, -285, 5, 0, LEFT, 4, 5, "Cubic eqn: power consumption of condenser fan as a function of condenser part load ratio"
;            COMBO, 14185, 14185, 751, 1, SYSTEM, 0,  REFG-AMB-COND-FT, 0, STD, 330, 230, 300, 225, 19, 3,    "Condenser Cap = f(ambient wetbulb temp):", LEFT, -285, 5, 0, LEFT, 4, 5, "Cubic eqn: fraction of condenser that is active as a fct of ambient temperature"
;            COMBO, 14184, 14184, 751, 1, SYSTEM, 0,  REFG-COND-CAP-FT, 0, STD, 330, 255, 300, 225, 19, 3, "Evap Condenser Cap = f(cond temp, osa wbt):", LEFT, -285, 5, 0, LEFT, 4, 5, "Bi-Quadratic eqn: Evap condenser capacity as fct of condensing wetbulb temp & OA wetbulb"
;            
;            CASE, SYSTEM, 0, REFG-HREC-STAGE2, -1, >, 1, 0
;               LABEL,      "Comp kW @stg2 HR =", STD, CENTER, 555,  46, 1, 0, 0, 0, 14189, 3
;               LABEL,      "f(condensing temp)", STD, CENTER, 555,  63, 1, 0, 0, 0, 14189, 3
;               COMBO, 14189, 14181, 751, 1, SYSTEM, 0, REFG-KW-HR-FTC, 0, STD, 475,  80, 300, 160, 19, 3,           "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic equation: compressor power as function of condensing temperature"
;               COMBO, 14187, 14181, 751, 1, SYSTEM, 0, REFG-KW-HR-FTC, 1, STD, 475, 105, 300, 160, 19, 3,           "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic equation: compressor power as function of condensing temperature"
;               COMBO, 14188, 14181, 751, 1, SYSTEM, 0, REFG-KW-HR-FTC, 2, STD, 475, 130, 300, 160, 19, 3,           "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic equation: compressor power as function of condensing temperature"
;            ENDCASE   
;         ENDCASE
;      
;         CASE, ELSE
;            CASE, SYSTEM, 0, REFG-HREC-STAGE2, -1, >, 1, 0
;               LABEL,      "Comp kW @stg2 HR =", STD, CENTER, 555,  46, 1, 0, 0, 0, 14190, 3
;               LABEL,      "f(condensing temp)", STD, CENTER, 555,  63, 1, 0, 0, 0, 14190, 3
;               COMBO, 14190, 14181, 751, 1, SYSTEM, 0, REFG-KW-HR-FTC, 0, STD, 475,  80, 300, 160, 19, 3,           "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic equation: compressor power as function of condensing temperature"
;               COMBO, 14191, 14181, 751, 1, SYSTEM, 0, REFG-KW-HR-FTC, 1, STD, 475, 105, 300, 160, 19, 3,           "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic equation: compressor power as function of condensing temperature"
;               COMBO, 14192, 14181, 751, 1, SYSTEM, 0, REFG-KW-HR-FTC, 2, STD, 475, 130, 300, 160, 19, 3,           "", LEFT,   -2, 5, 0, LEFT, 4, 5, "Cubic equation: compressor power as function of condensing temperature"
;            ENDCASE   
;         ENDCASE


; SAC 11/7/00 - Compliance keyword
    ;*****************************************
    ; COMPLIANCE
    ;*****************************************
    TABPAGE, 3228, 2013, 1, 7, NOTIMP, " Compliance "

; AFR 7/14/09 - changed name from Basic Specifications
       SUBTABPAGE, 3229, 2013, 1, 7, "  Compliance Reporting  "

; AFR 7/15/09 - moved to Basics tab per KJM
;          EDIT, 15543, 15543, 0, 1, SYSTEM, 0,   C-NUM-OF-UNITS, 0, STD, 175,  10,  23,  80,  0, 1,           "Number of Units:", LEFT, -150, 5, 1, LEFT, 4, 5, "The number of identical units"
; SAC 7/25/06 - added C-ELEC-PHASE and shifted all other controls in this column down by 25 - per KJM e-mail of 6/27/06
; AFR 7/15/09 - removed per KJM
;         COMBO, 18239, 18239, 0, 1, SYSTEM, 0,     C-ELEC-PHASE, 0, STD, 175,  35, 300, 145, 19, 1,         "Electricity Phase:", LEFT, -150, 5, 0, LEFT, 4, 5, "Package cooling system served by single- or three-phase electrical power"
; AFR 7/15/09 - moved to Basics tab per KJM
;         COMBO, 15557, 15557, 0, 1, SYSTEM, 0,    C-HAS-HTG-CLG, 0, STD, 175,  60, 300, 145, 19, 1,           "System Used For:", LEFT, -150, 5, 0, LEFT, 4, 5, "The type of system (heating/cooling/both)"
;         COMBO, 15549, 15549, 0, 1, SYSTEM, 0,    C-FURN-CONFIG, 0, STD, 175,  85, 300, 145, 19, 1,     "Furnace Configuration:", LEFT, -150, 5, 0, LEFT, 4, 5, "The configuration of the furnace"
;         COMBO, 15546, 15546, 0, 1, SYSTEM, 0,      C-HP-CONFIG, 0, STD, 175, 110, 300, 145, 19, 1,   "Heat Pump Configuration:", LEFT, -150, 5, 0, LEFT, 4, 5, "The configuration of the heat pump"
      CHECKBOX, 15547, 15547, 0, 1, SYSTEM, 0,      C-SUPP-HEAT, 0, STD,  50, 163,  18, 260,     7,  "Heat Pump Has Supplemental Heat", LEFT, "Checked if supplemental heat is installed for the heat pump"
      CHECKBOX, 15548, 15548, 0, 1, SYSTEM, 0,  C-HT-PUMP-TSTAT, 0, STD,  50, 188,  18, 260,     7,  "Heat Pump Has Thermostat",        LEFT, "Checked if the heat pump has a heat pump thermostat"

; AFR 7/15/09 - moved to Basics tab per KJM
;         COMBO, 15545, 15545, 0, 1, SYSTEM, 0,      C-AC-CONFIG, 0, STD, 175, 210, 300, 145, 19, 1,   "Air Cond. Configuration:", LEFT, -150, 5, 0, LEFT, 4, 5, "The configuration of the air conditioner"
         COMBO, 15550, 15550, 0, 1, SYSTEM, 0, C-CONDENSER-TYPE, 0, STD, 175, 235, 300, 145, 19, 7,            "Condenser Type:", LEFT, -150, 5, 0, LEFT, 4, 5, "The condenser type for the air conditioner"

          EDIT, 15544, 15544, 0, 1, SYSTEM, 0,  C-NUM-ISO-ZONES, 0, STD, 175, 260,  23,  80,  0, 7,   "Num. of Isolation Zones:", LEFT, -150, 5, 1, LEFT, 4, 5, "The number of isolation zones served by this system"
      CHECKBOX, 15558, 15558, 0, 1, SYSTEM, 0,  C-SYS-ZONE-TYPE, 0, STD,  25, 288,  18, 280,     7,  "System Serves Multiple Thermostatic Zones", LEFT, "The zoning configuration (single or multiple) of this system"

; SAC 1/18/06 - mods for T-24 2005
; AFR 7/15/09 - moved the following over to the left side of the dialog.
; SAC 1/6/10 - removed keywords no longer referenced by T24-08 ruleset (C-TXV-CERT & C-AIR-CERT)
;      CHECKBOX, 18220,     0, 0, 1, SYSTEM, 0,       C-TXV-CERT, 0, STD,  50,  10,  18, 200,     7, "Certified Refrigerant Charge", LEFT, ""
;      CHECKBOX, 18221,     0, 0, 1, SYSTEM, 0,       C-AIR-CERT, 0, STD,  50,  35,  18, 140,     7,            "Certified Airflow", LEFT, ""

         COMBO, 15551, 15551, 0, 1, SYSTEM, 0,   C-TIME-CONTROL, 0, STD, 170,  60, 300, 150, 19, 7,            "Time Control:", LEFT, -125, 5, 0, LEFT, 4, 5, "The type of time control for the system"
         COMBO, 15552, 15552, 0, 1, SYSTEM, 0,  C-SETBK-CONTROL, 0, STD, 170,  85, 300, 150, 19, 7,         "Setback Control:", LEFT, -125, 5, 0, LEFT, 4, 5, "The type of temperature setback(setup) control"

         COMBO, 15553, 15553, 0, 1, SYSTEM, 0,    C-VENT-METHOD, 0, STD, 170, 110, 300, 150, 19, 7,      "Ventilation Method:", LEFT, -125, 5, 0, LEFT, 4, 5, "The method for certifying correct amount of outside ventilation air"
      CHECKBOX, 15554, 15554, 0, 1, SYSTEM, 0,  C-OSA-DMPR-CTRL, 0, STD,  50, 138,  18, 270,     7, "Has Automatic Outside Air Damper Control", LEFT, "Checked if system has automatically controlled outside air dampers"

        SPREAD, 15556, 15556, 0, 1, 0, PowerDOE, 0, SysPipeTypeSpread,  0, STD, 370, 185, 140, 285, 19, 7, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""

; AFR 4/29/09 - moved ducts here from Basics
      LABEL, "Cooling/Heating Ducts (data used for compliance reporting only)", STD, LEFT, 25, 330, 1, 0, 0, 630, 15575, 7
      LABEL, "R-Value",  STD, LEFT, 105, 349, 1, 0, 0, 0, 15576, 7
      LABEL, "Location", STD, LEFT, 235, 349, 1, 0, 0, 0, 15584, 7
       EDIT, 15575, 15575, 0, 1, SYSTEM, 0,  C-CLG-DUCT-RVAL, -1, STD, 100, 369,  23,  60,  2, 7, "Cooling:", RIGHT,  -5, 5, 1, LEFT, 4, 5, "The insulation R-Value of the majority of the cooling ducts"
       EDIT, 15576, 15576, 0, 1, SYSTEM, 0,  C-CLG-DUCT-LOCN, -1, STD, 230, 369,  23, 340, 76, 7, "",         RIGHT,  -5, 5, 1, LEFT, 4, 5, "The location of the majority of the cooling ducts of the system"
       EDIT, 15584, 15584, 0, 1, SYSTEM, 0,  C-HTG-DUCT-RVAL, -1, STD, 100, 394,  23,  60,  2, 7, "Heating:", RIGHT,  -5, 5, 1, LEFT, 4, 5, "The insulation R-Value of the majority of the heating ducts"
       EDIT, 15585, 15585, 0, 1, SYSTEM, 0,  C-HTG-DUCT-LOCN, -1, STD, 230, 394,  23, 340, 76, 7, "",         RIGHT,  -5, 5, 1, LEFT, 4, 5, "The location of the majority of the heating ducts of the system"


; unused
; 433> C-ET-MAX                              Numnric Err,Cau    1            0.00            1.00 454  -77777.00 *No Default*    

; AFR 7/2/09 - incorporated data in Fans tab dialog.
;       SUBTABPAGE, 3230, 2013, 1, 1, "  Fans  "
;
;         LABEL, "Supply Fan(s)", STD, LEFT, 185, 1, 1, 0, 0, 325, 15521, 1
;          EDIT, 15521, 15521, 0, 1, SYSTEM, 0,    C-SUP-FAN-QTY, 0, STD, 185,  20,  23,  80,  0, 1,              "Number of Fans:", LEFT, -165, 5, 1, LEFT, 4, 5, "The total number of supply fans for all identical units"
;         COMBO, 15522, 15522, 0, 1, SYSTEM, 0,  C-SUPP-FAN-TYPE, 0, STD, 185,  44, 300, 140, 19, 1,                    "Fan Type:", LEFT, -165, 5, 0, LEFT, 4, 5, "The type or flow control of the supply fan"
;         COMBO, 15524, 15524, 0, 1, SYSTEM, 0,    C-SF-MTR-TYPE, 0, STD, 185,  68, 300, 140, 19, 1,   "Motor Efficiency Category:", LEFT, -165, 5, 0, LEFT, 4, 5, "The category describing the supply fan motor efficiency"
;         COMBO, 15523, 15523, 0, 1, SYSTEM, 0, C-SF-MTR-SNC-SPD, 0, STD, 185,  92, 300, 140, 19, 1,     "Motor Synchronous Speed:", LEFT, -165, 5, 0, LEFT, 4, 5, "The synchronous speed of the supply fan motor"
;; SAC 8/30/01 - Compliance keyword
;         COMBO, 17501, 17501, 0, 1, SYSTEM, 0,    C-SF-MTR-ENCL, 0, STD, 185, 116, 300, 140, 19, 1,        "Motor Enclosure Type:", LEFT, -165, 5, 0, LEFT, 4, 5, "The type of enclosure for the supply fan motor"
;          EDIT, 15525, 15525, 0, 1, SYSTEM, 0,  C-SF-TOT-NOM-HP, 0, STD, 185, 140,  23,  80,  1, 1,          "Nominal Horsepower:", LEFT, -165, 5, 1, LEFT, 4, 5, "The total supply fan nominal (nameplate) motor horsepower for all identical units"
;          EDIT, 15526, 15526, 0, 1, SYSTEM, 0,     C-SF-TOT-BHP, 0, STD, 185, 164,  23,  80,  2, 1,      "Total Brake Horsepower:", LEFT, -165, 5, 1, LEFT, 4, 5, "The total supply fan brake motor brake horsepower for all identical units"
;          EDIT, 15527, 15527, 0, 1, SYSTEM, 0,   C-SF-MOTOR-EFF, 0, STD, 185, 188,  23,  80,  3, 1,            "Motor Efficiency:", LEFT, -165, 5, 1, LEFT, 4, 5, "The efficiency of the supply fan motor"
;          EDIT, 15528, 15528, 0, 1, SYSTEM, 0,   C-SF-DRIVE-EFF, 0, STD, 185, 212,  23,  80,  3, 1,            "Drive Efficiency:", LEFT, -165, 5, 1, LEFT, 4, 5, "The efficiency of the supply fan drive"
;      CHECKBOX, 15529, 15529, 0, 1, SYSTEM, 0,  C-SF-FILTRATION, 0, STD, 186, 241,  18, 155,     1,    "Special Filtration Exists", LEFT,                         "Checked if specialized filtration exceeds 1 in. static pressure drop"
;          EDIT, 15530, 15530, 0, 1, SYSTEM, 0,     C-SF-FILT-SP, 0, STD, 185, 264,  23,  80,  2, 1,  "Filtration Static Pressure:", LEFT, -165, 5, 1, LEFT, 4, 5, "The pressure drop through the specialized supply filtration equipment"
;          EDIT, 15531, 15531, 0, 1, SYSTEM, 0,      C-SF-TOT-SP, 0, STD, 185, 285,  23,  80,  2, 1,       "Total Static Pressure:", LEFT, -165, 5, 1, LEFT, 4, 5, "The total static pressure of the supply air system"
;; SAC 12/22/00 - switched from SUPP to RET flow => moved to next column
;         EDIT, 15532, 15532, 0, 1, SYSTEM, 0,  C-TOT-SUPP-FLOW, 0, STD, 185, 309,  23,  80,  2, 1,                  "Total Flow:", LEFT, -165, 5, 1, LEFT, 4, 5, "The total supply air quantity of all identical units"
;
;         LABEL, "Return Fan(s)", STD, LEFT, 355, 1, 1, 0, 0, 495, 15521, 1
;          EDIT, 15533, 15533, 0, 1, SYSTEM, 0,    C-RET-FAN-QTY, 0, STD, 355,  20,  23,  80,  0, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The total number of return fans for all identical units"
;         COMBO, 15534, 15534, 0, 1, SYSTEM, 0,   C-RET-FAN-TYPE, 0, STD, 355,  44, 300, 140, 19, 1,                             "", LEFT,   -1, 5, 0, LEFT, 4, 5, "The type or flow control of the return fan"
;         COMBO, 15535, 15535, 0, 1, SYSTEM, 0,    C-RF-MTR-TYPE, 0, STD, 355,  68, 300, 140, 19, 1,                             "", LEFT,   -1, 5, 0, LEFT, 4, 5, "The category describing the return fan motor efficiency"
;         COMBO, 15536, 15536, 0, 1, SYSTEM, 0, C-RF-MTR-SNC-SPD, 0, STD, 355,  92, 300, 140, 19, 1,                             "", LEFT,   -1, 5, 0, LEFT, 4, 5, "The synchronous speed of the return fan motor"
;; SAC 8/30/01 - Compliance keyword
;         COMBO, 17502, 17502, 0, 1, SYSTEM, 0,    C-RF-MTR-ENCL, 0, STD, 355, 116, 300, 140, 19, 1,                             "", LEFT,   -1, 5, 0, LEFT, 4, 5, "The type of enclosure for the return fan motor"
;          EDIT, 15537, 15537, 0, 1, SYSTEM, 0,  C-RF-TOT-NOM-HP, 0, STD, 355, 140,  23,  80,  1, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The total return fan nominal (nameplate) motor horsepower for all identical units"
;          EDIT, 15538, 15538, 0, 1, SYSTEM, 0,     C-RF-TOT-BHP, 0, STD, 355, 164,  23,  80,  2, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The total return fan brake motor brake horsepower for all identical units"
;          EDIT, 15539, 15539, 0, 1, SYSTEM, 0,   C-RF-MOTOR-EFF, 0, STD, 355, 188,  23,  80,  3, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The efficiency of the return fan motor"
;          EDIT, 15540, 15540, 0, 1, SYSTEM, 0,   C-RF-DRIVE-EFF, 0, STD, 355, 212,  23,  80,  3, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The efficiency of the return fan drive"
;      CHECKBOX, 15541, 15541, 0, 1, SYSTEM, 0,  C-RF-FILTRATION, 0, STD, 356, 241,  18, 155,     1,    "Special Filtration Exists", LEFT,                         "Checked if specialized filtration exceeds 1 in. static pressure drop"
;          EDIT, 15542, 15542, 0, 1, SYSTEM, 0,     C-RF-FILT-SP, 0, STD, 355, 264,  23,  80,  2, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The pressure drop through the specialized return filtration equipment"
;          EDIT, 15543, 15543, 0, 1, SYSTEM, 0,      C-RF-TOT-SP, 0, STD, 355, 285,  23,  80,  2, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The total static pressure of the return air system"
;          EDIT, 15532, 15532, 0, 1, SYSTEM, 0,   C-TOT-RET-FLOW, 0, STD, 355, 309,  23,  80,  2, 1,                  "Total Flow:", LEFT, -335, 5, 1, LEFT, 4, 5, "The total return air quantity of all identical units"
;
;; SAC 7/13/04 - Added compliance heating fan keyword controls
;       CASE, SYSTEM, 0, DDS-TYPE, -1, =, 1, 2
;         LABEL, "Heating Fan(s)", STD, LEFT, 525, 1, 1, 0, 0, 665, 17855, 1
;          EDIT, 17855, 17855, 0, 1, SYSTEM, 0,       C-HFAN-QTY, 0, STD, 525,  20,  23,  80,  0, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The total number of heating fans for all identical units"
;         COMBO, 17856, 17856, 0, 1, SYSTEM, 0,      C-HFAN-TYPE, 0, STD, 525,  44, 300, 140, 19, 1,                             "", LEFT,   -1, 5, 0, LEFT, 4, 5, "The type or flow control of the heating fan"
;         COMBO, 17857, 17857, 0, 1, SYSTEM, 0,  C-HFAN-MTR-TYPE, 0, STD, 525,  68, 300, 140, 19, 1,                             "", LEFT,   -1, 5, 0, LEFT, 4, 5, "The category describing the heating fan motor efficiency"
;         COMBO, 17858, 17858, 0, 1, SYSTEM, 0,   C-HFAN-MTR-SPD, 0, STD, 525,  92, 300, 140, 19, 1,                             "", LEFT,   -1, 5, 0, LEFT, 4, 5, "The synchronous speed of the heating fan motor"
;         COMBO, 17859, 17859, 0, 1, SYSTEM, 0,  C-HFAB-MTR-ENCL, 0, STD, 525, 116, 300, 140, 19, 1,                             "", LEFT,   -1, 5, 0, LEFT, 4, 5, "The type of enclosure for the heating fan motor"
;          EDIT, 17860, 17860, 0, 1, SYSTEM, 0, C-HFAN-TOT-NM-HP, 0, STD, 525, 140,  23,  80,  1, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The total heating fan nominal (nameplate) motor horsepower for all identical units"
;          EDIT, 17861, 17861, 0, 1, SYSTEM, 0,   C-HFAN-TOT-BHP, 0, STD, 525, 164,  23,  80,  2, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The total heating fan brake motor brake horsepower for all identical units"
;          EDIT, 17862, 17862, 0, 1, SYSTEM, 0,   C-HFAN-MTR-EFF, 0, STD, 525, 188,  23,  80,  3, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The efficiency of the heating fan motor"
;          EDIT, 17863, 17863, 0, 1, SYSTEM, 0, C-HFAN-DRIVE-EFF, 0, STD, 525, 212,  23,  80,  3, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The efficiency of the heating fan drive"
;      CHECKBOX, 17864, 17864, 0, 1, SYSTEM, 0,  C-HF-FILTRATION, 0, STD, 526, 241,  18, 155,     1,    "Special Filtration Exists", LEFT,                         "Checked if specialized filtration exceeds 1 in. static pressure drop"
;          EDIT, 17865, 17865, 0, 1, SYSTEM, 0,     C-HF-FILT-SP, 0, STD, 525, 264,  23,  80,  2, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The pressure drop through the specialized heating filtration equipment"
;          EDIT, 17866, 17866, 0, 1, SYSTEM, 0,      C-HF-TOT-SP, 0, STD, 525, 285,  23,  80,  2, 1,                             "", LEFT,   -1, 5, 1, LEFT, 4, 5, "The total static pressure of the heating air system"
;       ENDCASE   
; Redundent keywords??:
;   522> C-HTG-FAN-QTY                         Numeric Rounded    1            0.00          100.00 681       1.00                 
;   527> C-HF-MTR-ENCL                         Numeric Rounded    1            0.00          100.00 686  -77777.00 *No Default*    

; AFR 4/29/09 - removed per Kevin/Luke
;       SUBTABPAGE, 3231, 2013, 1, 1, "  Cooling  "

; AFR 4/29/09 - moved to Cooling / Coil Cap / Control tab
;          EDIT, 15559, 15559, 0, 1, SYSTEM, 0,  C-TOTAL-CLG-CAP, 0, STD, 170,  15,  23,  95,  1, 1,      "Total Cooling Capacity:", LEFT, -145, 5, 1, LEFT, 4, 5, "The total cooling capacity of all identical units"

; SAC 4/23/09 - Moved to Cooling / Unitary Power tab
;         LABEL, "Efficiency Ratings:", STD, LEFT,  25, 60, 1, 0, 0, 310, 0, 1
;         LABEL, "FULL LOAD",           STD, LEFT, 320, 60, 1, 0, 0, 520, 0, 1
;         LABEL, "PART LOAD",           STD, LEFT, 530, 60, 1, 0, 0, 640, 0, 1
;
;         LABEL, "Seasonal Ratings (if applicable):",    STD, LEFT,  25,  85, 1, 0, 0, 0, 15562, 1
;         LABEL, "Air/Evaporatively Cooled DX Ratings:", STD, LEFT,  25, 110, 1, 0, 0, 0, 15560, 1
;         LABEL, "Water Cooled DX Ratings:",             STD, LEFT,  25, 135, 1, 0, 0, 0, 15567, 1
;         LABEL, "Ground Water Cooled DX Ratings:",      STD, LEFT,  25, 160, 1, 0, 0, 0, 15569, 1
;
;          EDIT, 15562, 15562, 0, 1, SYSTEM, 0,           C-SEER, 0, STD, 310,  80,  23,  80,  2, 1,                        "SEER:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The SEER of the air conditioner"
;          EDIT, 15561, 15561, 0, 1, SYSTEM, 0,           C-IPLV, 0, STD, 520,  80,  23,  80,  2, 1,                        "IPLV:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The IPLV of the air conditioner"
;          EDIT, 15560, 15560, 0, 1, SYSTEM, 0,          C-EER95, 0, STD, 310, 105,  23,  80,  2, 1,                      "EER 95:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 95F (ODB) of the air cooled air conditioner"
;          EDIT, 15566, 15566, 0, 1, SYSTEM, 0,          C-EER82, 0, STD, 520, 105,  23,  80,  2, 1,                      "EER 82:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 82F (ODB) of the air cooled air conditioner"
;          EDIT, 15567, 15567, 0, 1, SYSTEM, 0,       C-EER85EWT, 0, STD, 310, 130,  23,  80,  2, 1,                      "EER 85:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 85F (EWT) of the water source heat pump"
;          EDIT, 15568, 15568, 0, 1, SYSTEM, 0,       C-EER75EWT, 0, STD, 520, 130,  23,  80,  2, 1,                      "EER 75:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 75F (EWT) of the water source heat pump"
;          EDIT, 15569, 15569, 0, 1, SYSTEM, 0,       C-EER70EWT, 0, STD, 310, 155,  23,  80,  2, 1,                      "EER 70:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 70F (EWT) of the ground source heat pump"
;          EDIT, 15570, 15570, 0, 1, SYSTEM, 0,       C-EER50EWT, 0, STD, 520, 155,  23,  80,  2, 1,                      "EER 50:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The EER at 50F (EWT) of the ground source heat pump"

; AFR 4/29/09 - moved to Basics tab
;          EDIT, 15573, 15573, 0, 1, SYSTEM, 0, C-CLG-EQUIP-MFRG, -1, STD, 195, 210,  23, 455, 76, 1,   "Equipment Manufacturer(s):", LEFT, -170, 5, 1, LEFT, 4, 5, "The manufacturer of the primary cooling equipment of the system"
;          EDIT, 15574, 15574, 0, 1, SYSTEM, 0, C-CLG-EQUIP-MNUM, -1, STD, 195, 235,  23, 455, 76, 1,   "Equipment Model Number(s):", LEFT, -170, 5, 1, LEFT, 4, 5, "The model number of the primary cooling equipment of the system"

; AFR 7/15/09 - moved to Compliance Reporting
;         LABEL, "Cooling Ducts (data used for compliance reporting only)", STD, LEFT, 25, 275, 1, 0, 0, 650, 15575, 1
;          EDIT, 15575, 15575, 0, 1, SYSTEM, 0,  C-CLG-DUCT-RVAL, -1, STD, 100, 295,  23,  60,  2, 1,                     "R-Value:", RIGHT,  -5, 5, 1, LEFT, 4, 5, "The insulation R-Value of the majority of the cooling ducts"
;          EDIT, 15576, 15576, 0, 1, SYSTEM, 0,  C-CLG-DUCT-LOCN, -1, STD, 310, 295,  23, 340, 76, 1,                    "Location:", RIGHT,  -5, 5, 1, LEFT, 4, 5, "The location of the majority of the cooling ducts of the system"

; AFR 7/15/09 - nothing left, so hide this subtab.
;       SUBTABPAGE, 3232, 2013, 1, 1, "  Heating  "
;
; AFR 7/15/09 - moved to Heating/Unitary Power
;          EDIT, 15577, 15577, 0, 1, SYSTEM, 0,   C-TOTAL-HTG-CAP, 0, STD, 170,   5,  23,  95,  1, 1,           "Total Heating Capacity:", LEFT, -145, 5, 1, LEFT, 4, 5, "The total heating capacity of all identical units"
;          EDIT, 15581, 15581, 0, 1, SYSTEM, 0,  C-USER-INPUT-HIR, 0, STD, 520,   5,  23,  80,  3, 1,  "Pre-calculated Heat Input Ratio:", RIGHT,  -8, 5, 1, LEFT, 4, 5, "The user calculated HIR for multiple furnaces simulated as one system"
;
;         LABEL, "Efficiency Ratings:", STD, LEFT,  25, 45, 1, 0, 0, 310, 0, 1
;         LABEL, "FULL LOAD",           STD, LEFT, 320, 45, 1, 0, 0, 520, 0, 1
;         LABEL, "PART LOAD",           STD, LEFT, 530, 45, 1, 0, 0, 640, 0, 1
;
;         LABEL, "Seasonal Furnace Ratings:",            STD, LEFT,  25,  70, 1, 0, 0, 0, 15578, 1
;         LABEL, "Furnace Ratings:",                     STD, LEFT,  25,  95, 1, 0, 0, 0, 15579, 1
;         LABEL, "Seasonal Heat Pump Ratings:",          STD, LEFT,  25, 120, 1, 0, 0, 0, 15565, 1
;         LABEL, "Air-Cooled Heat Pump Ratings:",        STD, LEFT,  25, 145, 1, 0, 0, 0, 15563, 1
;         LABEL, "Water/Grnd Source Ht Pump Ratings:",   STD, LEFT,  25, 170, 1, 0, 0, 0, 15571, 1
;
;          EDIT, 15578, 15578, 0, 1, SYSTEM, 0,            C-AFUE, 0, STD, 310,  65,  23,  80,  2, 1,                        "AFUE:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The AFUE of the furnace"
;          EDIT, 15579, 15579, 0, 1, SYSTEM, 0,   C-THERM-EFF-MAX, 0, STD, 310,  90,  23,  80,  2, 1,                      "Et Max:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The thermal efficiency of the furnace at its maximum capacity"
;          EDIT, 15580, 15580, 0, 1, SYSTEM, 0,   C-THERM-EFF-MIN, 0, STD, 520,  90,  23,  80,  2, 1,                      "Et Min:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The thermal efficiency of the furnace at its minimum capacity"
;          EDIT, 15565, 15565, 0, 1, SYSTEM, 0,            C-HSPF, 0, STD, 310, 115,  23,  80,  2, 1,                        "HSPF:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The HSPF of the heat pump"
;          EDIT, 15563, 15563, 0, 1, SYSTEM, 0,           C-COP47, 0, STD, 310, 140,  23,  80,  2, 1,                      "COP 47:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The COP at 47F (ODB) of the air cooled heat pump"
;          EDIT, 15564, 15564, 0, 1, SYSTEM, 0,           C-COP17, 0, STD, 520, 140,  23,  80,  2, 1,                      "COP 17:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The COP at 17F (ODB) of the air cooled heat pump"
;          EDIT, 15571, 15571, 0, 1, SYSTEM, 0,        C-COP70EWT, 0, STD, 310, 165,  23,  80,  2, 1,                      "COP 70:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The COP at 70F (EWT) of the ground source heat pump"
;          EDIT, 15572, 15572, 0, 1, SYSTEM, 0,        C-COP50EWT, 0, STD, 520, 165,  23,  80,  2, 1,                      "COP 50:", LEFT,  -50, 5, 1, LEFT, 4, 5, "The COP at 50F (EWT) of the ground source heat pump"

; AFR 7/15/09 - moved to Basics tab.
;          EDIT, 15582, 15582, 0, 1, SYSTEM, 0, C-HTG-EQUIP-MFRG, -1, STD, 195, 210,  23, 455, 76, 1,   "Equipment Manufacturer(s):", LEFT, -170, 5, 1, LEFT, 4, 5, "The manufacturer of the primary heating equipment of the system"
;          EDIT, 15583, 15583, 0, 1, SYSTEM, 0, C-HTG-EQUIP-MNUM, -1, STD, 195, 235,  23, 455, 76, 1,   "Equipment Model Number(s):", LEFT, -170, 5, 1, LEFT, 4, 5, "The model number of the primary heating equipment of the system"

; AFR 7/15/09 - moved to the Compliance Reporting tab
;         LABEL, "Heating Ducts (data used for compliance reporting only)", STD, LEFT, 25, 275, 1, 0, 0, 650, 15584, 1
;          EDIT, 15584, 15584, 0, 1, SYSTEM, 0,  C-HTG-DUCT-RVAL, -1, STD, 100, 295,  23,  60,  2, 1,                     "R-Value:", RIGHT,  -5, 5, 1, LEFT, 4, 5, "The insulation R-Value of the majority of the heating ducts"
;          EDIT, 15585, 15585, 0, 1, SYSTEM, 0,  C-HTG-DUCT-LOCN, -1, STD, 310, 295,  23, 340, 76, 1,                    "Location:", RIGHT,  -5, 5, 1, LEFT, 4, 5, "The location of the majority of the heating ducts of the system"


       SUBTABPAGE, 3350, 2013, 1, 7, "  Small DX Ducts  "

      CHECKBOX, 15555, 15555, 0, 1, SYSTEM, 0,   C-DUCT-TAPE-OK,  0, STD,  32,  10,  18, 260,     7,  "Duct Tape Acceptable for Sealing Ducts",    LEFT,                         "Checked if duct tape is an acceptable sealant for the ducts"

; SAC 1/18/06 - mods for T-24 2005
;      CHECKBOX, 17503, 17503, 0, 1, SYSTEM, 0,   C-DUCT-SEALING,  0, STD,  35,  35,  18, 280,     7,  "Duct Sealing Credit Utilized",             LEFT,                         "Checked if duct sealing credit is utilized"
         COMBO, 17503,     0, 0, 1, SYSTEM, 0, C-DUCT-LOSS-METH,  0, STD, 175,  35, 300, 128, 19, 7,  "Duct Loss Sim. Method:",                    LEFT, -145, 5, 0, LEFT, 4, 5, ""

          EDIT, 17504, 17504, 0, 1, SYSTEM, 0, C-DUCT-LEAK-FRAC,  0, STD, 215,  60,  23,  70,  3, 7,  "Duct Leakage Fraction:",                    LEFT, -185, 5, 1, LEFT, 4, 5, "One minus the measured fraction of air leakage from the ductwork"
          EDIT, 17505, 17505, 0, 1, SYSTEM, 0,  C-SUP-DUCT-RVAL,  0, STD, 215,  85,  23,  70,  2, 7,  "Supply Duct Insulation R-Value:",           LEFT, -185, 5, 1, LEFT, 4, 5, "The R-Value of the supply duct insulation"
          EDIT, 17506, 17506, 0, 1, SYSTEM, 0,  C-RET-DUCT-RVAL,  0, STD, 215, 110,  23,  70,  2, 7,  "Return Duct Insulation R-Value:",           LEFT, -185, 5, 1, LEFT, 4, 5, "The R-Value of the return duct insulation"

; SAC 1/18/06 - mods for T-24 2005
         COMBO, 18223,     0, 0, 1, SYSTEM, 0,  C-DUCT-SERVICES,  0, STD, 500,  10, 300, 150, 19, 7,  "System Serves:",                            LEFT, -150, 5, 0, LEFT, 4, 5, "Name of the zone that contains the ducting and piping (and receives duct thermal losses)"
         COMBO, 18224,     0, 0, 1, SYSTEM, 0,  C-DUCT-AREA-METH, 0, STD, 500,  35, 300, 150, 19, 7,  "Duct Area Calc. Method:",                   LEFT, -150, 5, 0, LEFT, 4, 5, "Name of the zone that contains the ducting and piping (and receives duct thermal losses)"
          EDIT, 18225,     0, 0, 1, SYSTEM, 0,  C-DUCT-SUP-AREA,  0, STD, 520,  60,  23,  70,  2, 7,  "Supply Duct Area:",                         LEFT, -170, 5, 1, LEFT, 4, 5, "One minus the measured fraction of air leakage from the ductwork"
          EDIT, 18226,     0, 0, 1, SYSTEM, 0,  C-DUCT-RET-AREA,  0, STD, 520,  85,  23,  70,  2, 7,  "Return Duct Area:",                         LEFT, -170, 5, 1, LEFT, 4, 5, "The R-Value of the supply duct insulation"
          EDIT, 18227,     0, 0, 1, SYSTEM, 0,  C-DUCT-OA-FRAC,   0, STD, 520, 110,  23,  70,  2, 7,  "Frac. of All Ducts Outdoors:",              LEFT, -170, 5, 1, LEFT, 4, 5, "The R-Value of the return duct insulation"

         LABEL, "Supply Ducts", STD, LEFT,  30, 152, 1, 0, 0, 330, 18230, 7
        SPREAD, 18230,     0, 0, 1, 0, PowerDOE, 0, SysSupplyDuctSpread,  0, STD,  40, 170, 155, 290, 19, 7, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""

         LABEL, "Return Ducts", STD, LEFT, 350, 152, 1, 0, 0, 650, 18231, 7
        SPREAD, 18231,     0, 0, 1, 0, PowerDOE, 0, SysReturnDuctSpread,  0, STD, 360, 170, 155, 290, 19, 7, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""


; SAC 6/30/03 - Added new tab specific to SBD duct insulation & leakage
       SUBTABPAGE, 3358, 2013, 1, 4, "  SBD Duct Losses  "

         CASE, SYSTEM, 0, TYPE, -1, =, 1, 6   ; UVT  => NO duct loss stuff at all
              LABEL, "No SBD Duct Loss Analysis is applicable for this system type.", STD, CENTER, 335, 73, 1, 0, 0, 0, 0, 4
         ENDCASE

         CASE, SYSTEM, 0, TYPE, -1, =, 1, 7   ; UHT  => NO duct loss stuff at all
              LABEL, "No SBD Duct Loss Analysis is applicable for this system type.", STD, CENTER, 335, 73, 1, 0, 0, 0, 0, 4
         ENDCASE

         CASE, SYSTEM, 0, TYPE, -1, =, 1, 8   ; FPH  => NO duct loss stuff at all
              LABEL, "No SBD Duct Loss Analysis is applicable for this system type.", STD, CENTER, 335, 73, 1, 0, 0, 0, 0, 4
         ENDCASE

         CASE, SYSTEM, 0, TYPE, -1, =, 1, 9   ; FC   => NO duct loss stuff at all
              LABEL, "No SBD Duct Loss Analysis is applicable for this system type.", STD, CENTER, 335, 73, 1, 0, 0, 0, 0, 4
         ENDCASE

         CASE, SYSTEM, 0, TYPE, -1, =, 1, 15  ; HP   => NO duct loss stuff at all
              LABEL, "No SBD Duct Loss Analysis is applicable for this system type.", STD, CENTER, 335, 73, 1, 0, 0, 0, 0, 4
         ENDCASE

         CASE, SYSTEM, 0, TYPE, -1, =, 1, 22  ; PTAC => NO duct loss stuff at all
              LABEL, "No SBD Duct Loss Analysis is applicable for this system type.", STD, CENTER, 335, 73, 1, 0, 0, 0, 0, 4
         ENDCASE

         CASE, SYSTEM, 0, TYPE, -1, =, 1, 4   ; DDS  => Both cooling AND heating duct loss inputs applicable
              LABEL, "Analysis Options & Duct Zone", STD, LEFT, 25, 10, 1, 0, 0, 650, 17750, 4
           CHECKBOX, 17750, 17750, 0, 1,   SYSTEM, 0,         C-COMP-DUCT-INS,  0, STD,  50,  33,  18, 250,     4,  "Perform SBD Duct Insulation Analysis",      LEFT,                         ""
           CHECKBOX, 17751, 17751, 0, 1,   SYSTEM, 0,        C-COMP-DUCT-SEAL,  0, STD,  50,  58,  18, 235,     4,  "Perform SBD Duct Leakage Analysis",         LEFT,                         ""

            CASE, SYSTEM, 0, C-COMP-DUCT-INS, -1, >, 1, 0
              COMBO, 17752, 13104, 0, 1,   SYSTEM, 0,               DUCT-ZONE,  0, STD, 500,  30, 300, 150, 19, 4,  "Duct Zone:",                                LEFT,  -70, 5, 0, LEFT, 4, 5, "Name of the zone that contains the ducting and piping (and receives duct thermal losses)"
              LABEL, "Supply Air Ducts", STD, LEFT, 25, 92, 1, 0, 0, 650, 15584, 4
             SPREAD, 17754, 17754, 0, 1, 0, PowerDOE, 0, SysSBDCoolDuctSpread,  0, STD,  40, 110, 100, 610, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
             SPREAD, 17755, 17755, 0, 1, 0, PowerDOE, 0, SysSBDHeatDuctSpread,  0, STD,  40, 225, 100, 610, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
            ENDCASE
            CASE, SYSTEM, 0, C-COMP-DUCT-SEAL, -1, >, 1, 0
              COMBO, 17753, 13104, 0, 1,   SYSTEM, 0,               DUCT-ZONE,  0, STD, 500,  30, 300, 150, 19, 4,  "Duct Zone:",                                LEFT,  -70, 5, 0, LEFT, 4, 5, "Name of the zone that contains the ducting and piping (and receives duct thermal losses)"
              LABEL, "Supply Air Ducts", STD, LEFT, 25, 92, 1, 0, 0, 650, 15584, 4
             SPREAD, 17765, 17754, 0, 1, 0, PowerDOE, 0, SysSBDCoolDuctSpread,  0, STD,  40, 110, 100, 610, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
             SPREAD, 17766, 17755, 0, 1, 0, PowerDOE, 0, SysSBDHeatDuctSpread,  0, STD,  40, 225, 100, 610, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
            ENDCASE
         ENDCASE

         CASE, ELSE                           ; - all other system types -  => Only cooling duct loss inputs applicable
              LABEL, "Analysis Options & Duct Zone", STD, LEFT, 25, 10, 1, 0, 0, 650, 17750, 4
           CHECKBOX, 17758, 17750, 0, 1,   SYSTEM, 0,         C-COMP-DUCT-INS,  0, STD,  50,  33,  18, 250,     4,  "Perform SBD Duct Insulation Analysis",      LEFT,                         ""
           CHECKBOX, 17759, 17751, 0, 1,   SYSTEM, 0,        C-COMP-DUCT-SEAL,  0, STD,  50,  58,  18, 235,     4,  "Perform SBD Duct Leakage Analysis",         LEFT,                         ""

            CASE, SYSTEM, 0, C-COMP-DUCT-INS, -1, >, 1, 0
              COMBO, 17760, 13104, 0, 1,   SYSTEM, 0,               DUCT-ZONE,  0, STD, 500,  30, 300, 150, 19, 4,  "Duct Zone:",                                LEFT,  -70, 5, 0, LEFT, 4, 5, "Name of the zone that contains the ducting and piping (and receives duct thermal losses)"
              LABEL, "Supply Air Ducts", STD, LEFT, 25, 92, 1, 0, 0, 650, 15584, 4
             SPREAD, 17762, 17754, 0, 1, 0, PowerDOE, 0, SysSBDCoolDuctSpread,  0, STD,  40, 110, 215, 610, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
            ENDCASE
            CASE, SYSTEM, 0, C-COMP-DUCT-SEAL, -1, >, 1, 0
              COMBO, 17761, 13104, 0, 1,   SYSTEM, 0,               DUCT-ZONE,  0, STD, 500,  30, 300, 150, 19, 4,  "Duct Zone:",                                LEFT,  -70, 5, 0, LEFT, 4, 5, "Name of the zone that contains the ducting and piping (and receives duct thermal losses)"
              LABEL, "Supply Air Ducts", STD, LEFT, 25, 92, 1, 0, 0, 650, 15584, 4
             SPREAD, 17768, 17754, 0, 1, 0, PowerDOE, 0, SysSBDCoolDuctSpread,  0, STD,  40, 110, 215, 610, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
            ENDCASE
         ENDCASE


 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Loop Parameters - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODTABDLG, 3061, 32064, 1, 100, 100, 310, 610, 0, CIRCULATION-LOOP, "Loop Name:  ", CIRCULATION-LOOP, 0, NAME, 0, 0, 0, "     Loop Type:  ", CIRCULATION-LOOP, 0, TYPE, 0, 0, 0, ""
 MODTABDLG, 3061, 32064, 1, 30, 30, 470, 710, 0, CIRCULATION-LOOP, "Circulation Loop Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added for circ loops similar to other "Currently Active" help items for other commands
   COMBO, 12188, 32064, 0, 1, CIRCULATION-LOOP, 0, NAME,  0, STD, 215,  15, 400, 250, 19, 3, "Currently Active Circulation Loop:",  LEFT, -200, 5, 0, LEFT, 4, 5, "List of all circulation loops defined in project; also allows library retrieval and creation"
   STATIC, 1, CIRCULATION-LOOP, 0, TYPE, 0, 0, 0, 485, 20, 250, STD, LEFT, "Type: ",   "", 0, 3

    ;******************************************
    ; Loops - Loop Parameters Page
    ;******************************************
    TABPAGE, 3069, 32064, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 12776, 12776, 0, 1, CIRCULATION-LOOP, 0,             NAME,  0, STD, 130,  25,  23, 180, 32, 3,                   "Loop Name:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Name of circulation loop; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 12777, 12777, 0, 1, CIRCULATION-LOOP, 0,             TYPE,  0, STD, 160,  50, 300, 150, 19, 3,                   "Loop Type:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Each loop must be one of six available types"
      COMBO, 12778, 12778, 0, 1, CIRCULATION-LOOP, 0,          SUBTYPE,  0, STD, 160,  75,  80, 150, 19, 3,                "Loop Subtype:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Secondary loops are served exclusively by primary loops"

      COMBO, 12851, 12851, 0, 1, CIRCULATION-LOOP, 0,        LOOP-PUMP,  0, STD, 160, 230, 350, 150, 19, 3,          "Loop Pump:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Name of the dedicated Pump that pumps this loop"
; SAC 1/16/06 - Design sizing mods
       EDIT, 19266,     0, 0, 1, CIRCULATION-LOOP, 0,        LOOP-FLOW, -1, STD, 160, 255,  23,  60,  1, 3,   "Design Loop Flow:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Design flowrate through the loop; cannot be smaller than design-day flow"
       EDIT, 13773, 12786, 0, 1, CIRCULATION-LOOP, 0,    LOOP-MIN-FLOW, -1, STD, 160, 280,  23,  60,  2, 3,  "Loop Minimum Flow:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Minimum allowable flow rate in the loop, expressed as a fraction of the design flow rate"
       EDIT, 12273, 12783, 0, 1, CIRCULATION-LOOP, 0, LOOP-RECIRC-FLOW, -1, STD, 160, 305,  23,  60,  1, 3,   "Loop Recirc Flow:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Recirculating flow rate of the fluid in the loop when the pump is running"
       EDIT, 12274, 12784, 0, 1, CIRCULATION-LOOP, 0,        PIPE-HEAD, -1, STD, 160, 330,  23,  60,  1, 3,          "Pipe Head:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Friction loss in the loop due to the piping and related trim"
       EDIT, 12275, 12785, 0, 1, CIRCULATION-LOOP, 0,      STATIC-HEAD, -1, STD, 160, 355,  23,  60,  1, 3,        "Static Head:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Loop static head (independent of the fluid flow rate)"
;     COMBO, 13775, 12788, 0, 1, CIRCULATION-LOOP, 0,       BRINE-TYPE,  0, STD, 160, 305, 110, 100, 19, 3,         "Brine Type:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The type of fluid circulating in the loop"
;      EDIT, 13776, 12789, 0, 1, CIRCULATION-LOOP, 0,        BRINE-PCT, -1, STD, 160, 210,  23,  60,  1, 3,      "Brine Percent:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The percent (by weight) of the glycol or salt in the working fluid of the loop"
;     COMBO, 13777, 12790, 0, 1, CIRCULATION-LOOP, 0,        COST-DATA,  0, STD, 160, 235, 120, 138, 19, 3,               "Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""


      COMBO, 12267, 12779, 0, 1, CIRCULATION-LOOP, 0,    SIZING-OPTION,  0, STD, 510, 115,  80, 140, 19, 3,               "Sizing Option:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Whether the loop is sized based on the loads it serves or the equipment that serves it"
; SAC 11/30/10 - added for DOE-2.3
      COMBO, 19260, 19260, 0, 1, CIRCULATION-LOOP, 0,    SIZING-WINDOW,  0, STD, 510, 140,  80, 140, 19, 3,               "Sizing Window:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Size equipment to load when actually used, or to maximum loop peak"
       EDIT, 13774, 12787, 0, 1, CIRCULATION-LOOP, 0,  LOOP-SIZE-RATIO, -1, STD, 510, 165,  23,  60,  1, 3,             "Loop Size Ratio:",  LEFT, -120, 5, 1, LEFT, 4, 5, "A safety factor applied to the primary equipment (e.g., boilers, etc.) in the loop sizing routine"
; SAC 8/19/03 - Added DESIGN-COOL-T and DESIGN-HEAT-T edit controls
       EDIT, 12268,     0, 0, 1, CIRCULATION-LOOP, 0,    DESIGN-COOL-T, -1, STD, 510, 190,  23,  60,  1, 3,             "Design CHW Temp:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Design chilled water temperature of the fluid in the loop"
       EDIT, 12269,     0, 0, 1, CIRCULATION-LOOP, 0,    DESIGN-HEAT-T, -1, STD, 510, 215,  23,  60,  1, 3,              "Design HW Temp:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Design hot water temperature of the fluid in the loop"
       EDIT, 12270, 12780, 0, 1, CIRCULATION-LOOP, 0,   LOOP-DESIGN-DT, -1, STD, 510, 240,  23,  60,  1, 3,              "Loop Design DT:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Design temperature change of the fluid in the loop"
       EDIT, 12271, 12781, 0, 1, CIRCULATION-LOOP, 0,     FLUID-VOLUME, -1, STD, 510, 265,  23,  60,  0, 3,                "Fluid Volume:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Total volume of the fluid in the loop"
       EDIT, 12272, 12782, 0, 1, CIRCULATION-LOOP, 0,    AVG-CIRC-TIME, -1, STD, 510, 290,  23,  60,  1, 3,               "Avg Circ Time:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Average time it takes for the fluid to circulate through the loop (at the design flow rate)"

; SAC 10/24/00 - Compliance Input
; SAC 8/19/03 - Moved from bottom of left column to bottom of right to accomodate DESIGN-*-T edits added above
      LABEL, "Compliance Settings", STD, LEFT, 370, 305, 0, 0, 1, 595, 15490, 1
       EDIT, 15490,     0, 0, 1, CIRCULATION-LOOP, 0,  C-TWR-PIPE-SIZE, -1, STD, 520, 325,  23,  60,  2, 1,       "Tower Inlet Pipe Size:",  LEFT, -135, 5, 1, LEFT, 4, 5, "The size of the condenser water pipe at the cooling tower inlet"

; SDG 10/06/13 - added for DOE-2.3
   CASE, CIRCULATION-LOOP, 0,    TYPE, -1, =, 2, 7,9
       EDIT, 18113,     0, 0, 1, CIRCULATION-LOOP, 0, DOWNSTREAM-SPLIT, -1, STD, 160, 140,  23,  60,  3, 3,            "Downstream Split:",  LEFT, -130, 5, 1, LEFT, 4, 5, "For equipment in series, the fraction of peak load assigned to series-downsteam equipment"
      COMBO, 18114,     0, 0, 1, CIRCULATION-LOOP, 0,    SERIES-BYPASS,  0, STD, 160, 165, 100, 150, 19, 3,               "Series Bypass:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Yes means Waterside economizer or equipment in series will be bypassed when inactive"
      COMBO, 18115,     0, 0, 1, CIRCULATION-LOOP, 0,      GLHX-BYPASS,  0, STD, 160, 190, 100, 150, 19, 3,                 "GLHX Bypass:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Yes means hybrid GLHX will be bypassed when inactive"
   ENDCASE   

   CASE, CIRCULATION-LOOP, 0, SUBTYPE, -1, =, 1, 1
; SAC 11/30/10 - added for DOE-2.3
      COMBO, 19265,     0, 0, 1, CIRCULATION-LOOP, 0,     EQUIP-CONFIG,  0, STD, 160, 115,  80, 150, 19, 3,            "Equipment Config:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Multiple equipment units may be in parallel, series, or series/parallel"
; SDG 10/06/13 - added for DOE-2.3
       EDIT, 12268,     0, 0, 1, CIRCULATION-LOOP, 0, DOWNSTREAM-SPLIT, -1, STD, 160, 140,  23,  60,  3, 3,            "Downstream Split:",  LEFT, -130, 5, 1, LEFT, 4, 5, "For equipment in series, the fraction of peak load assigned to series-downsteam equipment"
      COMBO, 18111,     0, 0, 1, CIRCULATION-LOOP, 0,    SERIES-BYPASS,  0, STD, 160, 165, 100, 150, 19, 3,               "Series Bypass:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Yes means Waterside economizer or equipment in series will be bypassed when inactive"
      COMBO, 18112,     0, 0, 1, CIRCULATION-LOOP, 0,      GLHX-BYPASS,  0, STD, 160, 190, 100, 150, 19, 3,                 "GLHX Bypass:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Yes means hybrid GLHX will be bypassed when inactive"

   ENDCASE   
   
   CASE, CIRCULATION-LOOP, 0, SUBTYPE, -1, =, 1, 2
      COMBO, 19144, 19143, 0, 1, CIRCULATION-LOOP, 0,     PRIMARY-LOOP,  0, STD, 160, 115, 350, 150, 19, 3,       "Primary Loop:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Name of the primary loop that this secondary loop is attached to (and served by)"
       EDIT, 12790, 14509, 0, 1, CIRCULATION-LOOP, 0, PRIMARY-FLOW-PCT, -1, STD, 160, 140,  23,  60,  1, 3, "% Trans to Primary:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Percentage of secondary loop flow that transfers to primary loop flow (at design conditions)"    
      COMBO, 12276, 12812, 0, 1, CIRCULATION-LOOP, 0,   VALVE-TYPE-2ND,  0, STD, 160, 165,  80, 150, 19, 3,         "Valve Type:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Type of valve that meters the primary fluid into the secondary loop or heat-exchanger"
       EDIT, 12277, 12884, 0, 1, CIRCULATION-LOOP, 0,   VALVE-HEAD-2ND, -1, STD, 160, 190,  23,  60,  1, 3,         "Valve Head:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Head loss of fluid across the valve that meters the flow between primary and secondary loops"    
;      EDIT, 12276, 12885, 0, 1, CIRCULATION-LOOP, 0,           NOTIMP, -1, STD, 510, 260,  23,  60,  1, 3, "Primary HX Delta T:",  LEFT, -130, 5, 1, LEFT, 4, 5,  8, ""    
;      EDIT, 12277, 12886, 0, 1, CIRCULATION-LOOP, 0,           NOTIMP, -1, STD, 510, 285,  23,  60,  1, 3,    "Primary HX Head:",  LEFT, -130, 5, 1, LEFT, 4, 5, 15, ""    
;     COMBO, 12278, 12888, 0, 1, CIRCULATION-LOOP, 0,           NOTIMP,  0, STD, 510, 310, 120, 100, 19, 3,     "Prim. Transfer:",  LEFT, -130, 5, 1, LEFT, 4, 5,    ""
;     COMBO, 12279, 12788, 0, 1, CIRCULATION-LOOP, 0,       BRINE-TYPE,  0, STD, 510, 330, 110, 100, 19, 3,         "Brine Type:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The type of fluid circulating in the loop"
;      EDIT, 12280, 12789, 0, 1, CIRCULATION-LOOP, 0,        BRINE-PCT, -1, STD, 510, 355,  23,  60,  1, 3,      "Brine Percent:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The percent (by weight) of the glycol or salt in the working fluid of the loop"
   ENDCASE                                                                         
   
    ;******************************************
    ; Loop Parameters - Process / DHW Loads Page
    ;******************************************
; SAC 10/24/00 - Added entire Process/DHW tab - plus compliance inputs
    TABPAGE, 3227, 32064, 1, 3, NOTIMP, " Process / DHW Loads "

      LABEL, "Process Loads / Flow", STD, LEFT, 30,  22, 0, 0, 1, 650, 14531, 3
     SPREAD, 14531,   992, 0, 1, 0, PowerDOE, 0, CircLoopProcessSpread,  0, STD, 100,  40, 140, 550, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 0, 0, ""

      LABEL, "Domestic Hot Water",   STD, LEFT, 30, 200, 0, 0, 1, 650, 12870, 3
       EDIT, 12870, 12870, 0, 1, CIRCULATION-LOOP, 0,      DHW-INLET-T, -1, STD, 165, 220,  23,  60,  1, 3, "Inlet Temperature:",           LEFT, -115,  5, 1, LEFT, 4, 5, "Inlet temperature of the potable water supplied to the DHW heater"
      COMBO, 12871, 12871, 0, 1, CIRCULATION-LOOP, 0,  DHW-INLET-T-SCH,  0, STD, 450, 220, 300, 200, 19, 3, "Inlet Temperature Schedule:", RIGHT,   -5,  5, 0, LEFT, 4, 5, "Scheduled inlet temperature of the potable water supplied to the DHW heater"

      LABEL, "DHW Compliance",   STD, LEFT, 30, 270, 0, 0, 1, 650, 15491, 1
       EDIT, 15491,     0, 0, 1, CIRCULATION-LOOP, 0,   C-NUM-DHW-HTRS, -1, STD, 165, 290,  23,  80,  0, 1, "Number of Heaters:",           LEFT, -115,  5, 1, LEFT, 4, 5, "The total number of direct fired water heaters attached to this circulation loop"
       EDIT, 15494,     0, 0, 1, CIRCULATION-LOOP, 0,    C-TOT-DHW-CAP, -1, STD, 165, 315,  23,  80,  1, 1, "Total Capacity:",              LEFT, -115,  5, 1, LEFT, 4, 5, "The total capacity of all direct fired water heaters attached to this circulation loop"
      COMBO, 15495,     0, 0, 1, CIRCULATION-LOOP, 0,   C-RES-DHW-TYPE,  0, STD, 165, 340, 300, 150, 19, 1, "Res. DHW Type:",               LEFT, -115,  5, 0, LEFT, 4, 5, "The type of residential DHW circulation system"
       EDIT, 15492,     0, 0, 1, CIRCULATION-LOOP, 0,   C-DHW-TANK-VOL, -1, STD, 520, 290,  23,  70,  1, 1, "Tank Volume:",                 LEFT, -105,  5, 1, LEFT, 4, 5, "The tank volume of the indirect fired water heating tank"
       EDIT, 15493,     0, 0, 1, CIRCULATION-LOOP, 0,  C-TANK-INS-RVAL, -1, STD, 520, 315,  23,  70,  1, 1, "Tank Ins. R-val:",             LEFT, -105,  5, 1, LEFT, 4, 5, "The R-Value of the insulation on the indirect fired water heating tank"


    ;******************************************
    ; Loop Parameters - Losses Page
    ;******************************************
    TABPAGE, 3062, 29056, 1, 3, NOTIMP, " Losses "

     EDIT, 13727, 12816, 0, 1, CIRCULATION-LOOP, 0,        SUPPLY-UA, -1, STD, 175,  22,  23,  55,  1, 3,          "Supply UA:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Thermal conductivity of the loop on the supply side (from entering loop to attached coils, etc.)"
     EDIT, 13728, 12817, 0, 1, CIRCULATION-LOOP, 0,   SUPPLY-LOSS-DT, -1, STD, 175,  47,  23,  55,  1, 3,     "Supply Loss DT:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Temperature change in the working fluid of the loop on the supply side "
; SAC 11/30/10 - added for DOE-2.3
     EDIT, 19271,     0, 0, 1, CIRCULATION-LOOP, 0,  SUPPLY-ENVIR-TD, -1, STD, 175,  72,  23,  55,  1, 3,  "Supply/Ambient TD:",  LEFT, -125, 5, 1, LEFT, 4, 5, "The log-mean temperature between the supply leg and the loop environment"
     EDIT, 17888, 12818, 0, 1, CIRCULATION-LOOP, 0,        RETURN-UA, -1, STD, 175,  97,  23,  55,  1, 3,          "Return UA:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Thermal conductivity of the loop on the return side"
     EDIT, 13730, 12819, 0, 1, CIRCULATION-LOOP, 0,   RETURN-LOSS-DT, -1, STD, 175, 122,  23,  55,  1, 3,     "Return Loss DT:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Temperature change in the working fluid of the loop on the return side "
; SAC 11/30/10 - added for DOE-2.3
     EDIT, 19272,     0, 0, 1, CIRCULATION-LOOP, 0,  RETURN-ENVIR-TD, -1, STD, 175, 147,  23,  55,  1, 3,  "Return/Ambient TD:",  LEFT, -125, 5, 1, LEFT, 4, 5, "The log-mean temperature between the return leg and the loop environment"
;     EDIT, 13731, 12820, 0, 1, CIRCULATION-LOOP, 0,  COOLING-ENVIR-T, -1, STD, 175, 122,  23,  55,  1, 3,  "Cool Environ Temp:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Design temperature of the pipe's environment when the loop is in cooling mode"   ; SAC 11/24/10 - removed
;     EDIT, 13732, 12821, 0, 1, CIRCULATION-LOOP, 0,  HEATING-ENVIR-T, -1, STD, 175, 147,  23,  55,  1, 3,  "Heat Environ Temp:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Design temperature of the pipe's environment when the loop is in heating mode"   ; SAC 11/24/10 - removed
                                                                                    
    COMBO, 13733, 12822, 0, 1, CIRCULATION-LOOP, 0,        LOOP-LOCN,  0, STD, 435,  22, 110, 135, 19, 3,      "Loop Location:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Location of the loop piping (determines the temperature at which losses occur)"
     EDIT, 13734, 12823, 0, 1, CIRCULATION-LOOP, 0,    LOOP-TUNNEL-T, -1, STD, 435,  47,  23,  50,  1, 3, "Tunnel Temperature:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""
    COMBO, 13735, 12824, 0, 1, CIRCULATION-LOOP, 0,  LOOP-TUNNEL-SCH, -1, STD, 435,  72, 200, 135, 19, 3,         "Tunnel Sch:",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
    COMBO, 13736, 12825, 0, 1, CIRCULATION-LOOP, 0,   LOOP-LOSS-ZONE, -1, STD, 435,  97, 200, 135, 19, 3,          "Loss Zone:",  LEFT, -130, 5, 0, LEFT, 4, 5, "The zone that the loop is in (the loop's thermal losses appear a loads in this zone)"
;    COMBO, 13737, 12826, 0, 1, CIRCULATION-LOOP, 0,  LOSSES-BASED-ON, -1, STD, 435, 122,  80, 135, 19, 3,     "Base Losses on:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Whether design loop thermal losses are based on heating or cooling mode of operation"   ; SAC 11/24/10 - removed
    COMBO, 14508, 14508, 0, 1, CIRCULATION-LOOP, 0, ASSIGN-LOSSES-TO, -1, STD, 435, 147,  80, 135, 19, 3,   "Assign Losses to:",  LEFT, -130, 5, 0, LEFT, 4, 5, "The end-use category in which the loop thermal losses are included in output reports"

; SAC 7/1/03 - Moved above controls up by 10 and added SBD piping losses spreadsheets
      CASE, CIRCULATION-LOOP, 0, TYPE, -1, =, 1, 1   ; CHW Loops
         CASE, COMPLIANCE, 0, C-COMP-PIPE-LOSS, -1, >, 1, 0
             LABEL, "Supply Piping Insulation", STD, LEFT,  25, 198, 1, 0, 0, 335, 0, 4
             SPREAD, 17775, 17775, 0, 1, 0, PowerDOE, 0, CircLoopSBDSupplyPipingSpread,  0, STD,  25, 215, 155, 310, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
             LABEL, "Return Piping Insulation", STD, LEFT, 370, 198, 1, 0, 0, 680, 0, 4
             SPREAD, 17776, 17776, 0, 1, 0, PowerDOE, 0, CircLoopSBDReturnPipingSpread,  0, STD, 370, 215, 155, 310, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
         ENDCASE
         CASE, ELSE
                 LABEL, "Note:  SBD pipe loss analysis can be toggled on from the Compliance component dialog.", STD, LEFT, 30, 215, 1, 0, 0, 0, 0, 4
         ENDCASE
      ENDCASE
      CASE, CIRCULATION-LOOP, 0, TYPE, -1, =, 1, 4   ; HW Loops
         CASE, COMPLIANCE, 0, C-COMP-PIPE-LOSS, -1, >, 1, 0
             LABEL, "Supply Piping Insulation", STD, LEFT,  25, 198, 1, 0, 0, 335, 0, 4
             SPREAD, 17777, 17775, 0, 1, 0, PowerDOE, 0, CircLoopSBDSupplyPipingSpread,  0, STD,  25, 215, 155, 310, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
             LABEL, "Return Piping Insulation", STD, LEFT, 370, 198, 1, 0, 0, 680, 0, 4
             SPREAD, 17778, 17776, 0, 1, 0, PowerDOE, 0, CircLoopSBDReturnPipingSpread,  0, STD, 370, 215, 155, 310, 19, 4, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""
         ENDCASE
         CASE, ELSE
                 LABEL, "Note:  SBD pipe loss analysis can be toggled on from the Compliance component dialog.", STD, LEFT, 30, 215, 1, 0, 0, 0, 0, 4
         ENDCASE
      ENDCASE

                                                                                                                                                         
    ;******************************************
    ; Loop Parameters - Head Page
    ;******************************************
    TABPAGE, 3063, 29057, 1, 3, NOTIMP, " Head "

      COMBO, 13738, 12830, 0, 1, CIRCULATION-LOOP, 0,  HEAD-SETPT-CTRL,  0, STD, 210,  32,  80, 115, 19, 3, "Head Setpoint Control:", LEFT, -160, 5, 0, LEFT, 4, 5, "Type of control sequence used to control the head setpoint of the loop circulation pumps"
      COMBO, 13739, 12831, 0, 1, CIRCULATION-LOOP, 0, HEAD-SENSOR-LOCN,  0, STD, 210,  57, 100, 115, 19, 3,  "Head Sensor Location:", LEFT, -160, 5, 0, LEFT, 4, 5, "Location of the differential head pressure sensor"
       EDIT, 13740, 12832, 0, 1, CIRCULATION-LOOP, 0,       HEAD-SETPT, -1, STD, 210,  82,  23,  50,  1, 3,         "Head Setpoint:", LEFT, -160, 5, 1, LEFT, 4, 5, "Design setpoint of the differential head pressure sensor"
       EDIT, 13741, 12833, 0, 1, CIRCULATION-LOOP, 0,   HEAD-SETPT-RNG, -1, STD, 210, 107,  23,  50,  1, 3,   "Head Setpoint Range:", LEFT, -160, 5, 1, LEFT, 4, 5, "Throttling range of the head setpoint controller"
       EDIT, 13742, 12834, 0, 1, CIRCULATION-LOOP, 0, HEAD-SETPT-RATIO, -1, STD, 210, 132,  23,  50,  1, 3,   "Head Setpoint Ratio:", LEFT, -160, 5, 1, LEFT, 4, 5, "A safety factor applied to the default Head Setpoint"

    ;******************************************
    ; Loop Parameters - Operation Page
    ;******************************************
    TABPAGE, 3066, 29058, 1, 3, NOTIMP, " Operation "

      COMBO, 13743, 12838, 0, 1, CIRCULATION-LOOP, 0,        SNAP-LOCN,  0, STD, 155,  32,  80, 140, 19, 3,    "Snap Location:",  LEFT, -105, 5, 0, LEFT, 4, 5, "Location of the snap-acting temperature sensor that turns the loop on or off"
       EDIT, 13744, 12839, 0, 1, CIRCULATION-LOOP, 0,           SNAP-T, -1, STD, 155,  57,  23,  50,  1, 3,        "Snap Temp:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Temperature at which the snap occurs (i.e., at which the Loop turns on or off)"
      COMBO, 13749, 12844, 0, 1, CIRCULATION-LOOP, 0,        SNAP-ZONE,  0, STD, 155,  82, 200, 140, 19, 3,        "Snap Zone:",  LEFT, -105, 5, 0, LEFT, 4, 5, "The zone whose temperature is monitored to determine whether the loop is active"

      COMBO, 13745, 12840, 0, 1, CIRCULATION-LOOP, 0,   LOOP-OPERATION,  0, STD, 455,  32, 110, 140, 19, 3,   "Loop Operation:",  LEFT, -120, 5, 0, LEFT, 4, 5, "Specifies when the loop is active"
      COMBO, 13746, 12841, 0, 1, CIRCULATION-LOOP, 0, COOLING-SCHEDULE,  0, STD, 455,  57, 200, 140, 19, 3, "Cooling Schedule:",  LEFT, -120, 5, 0, LEFT, 4, 5, "Specifies when the primary cooling or heat-rejection equipment is enabled"
      COMBO, 13747, 12842, 0, 1, CIRCULATION-LOOP, 0, HEATING-SCHEDULE,  0, STD, 455,  82, 200, 140, 19, 3, "Heating Schedule:",  LEFT, -120, 5, 0, LEFT, 4, 5, "Specifies when the primary heating equipment is enabled"
      COMBO, 13748, 12843, 0, 1, CIRCULATION-LOOP, 0,    PUMP-SCHEDULE,  0, STD, 455, 107, 200, 140, 19, 3,    "Pump Schedule:",  LEFT, -120, 5, 0, LEFT, 4, 5, "Specifies when the loop's pump is enabled"
                                                                                      
    ;******************************************
    ; Loop Parameters - Controls Page
    ;******************************************
    TABPAGE, 3067, 29022, 1, 3, NOTIMP, " Controls "

       EDIT, 13750, 12764, 0, 1, CIRCULATION-LOOP, 0, LOOP-FLOW-RESET, -1, STD, 145,   5,  23,  50,  3, 3,       "Loop Flow Reset:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Fraction of design flow rate to which the flow is reduced, prior to initiating a temperature reset "
       EDIT, 13761, 12765, 0, 1, CIRCULATION-LOOP, 0,  LOOP-SETPT-RNG, -1, STD, 145,  30,  23,  50,  1, 3,      "Loop Setpt Range:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Throttling range of the loop temperature controller"
       
     BUTTON, 10292, 10292, 0, 1, 92, 3096, STD, 420,   2, 23, 140, 3, "Equipment Controls", "Examine Equipment Controls"
     BUTTON, 10315, 10315, 0, 1, 92, 3125, STD, 570,   2, 23, 125, 3,    "Load Management", "Examine Load Management"

; SAC 11/30/10 - added for DOE-2.3
      COMBO, 19268,     0, 0, 1, CIRCULATION-LOOP, 0, LOAD-RESET-MODE,  0, STD, 530,  35, 110, 150, 19, 3,       "Load Reset Mode:",  LEFT, -115, 5, 0, LEFT, 4, 5, "For LOAD-RESET, whether equipment should be minimized or temperature reset (and flow) maximized"

      LABEL, "Heating", STD, LEFT, 30, 75, 0, 0, 1, 330, 13751, 3
      COMBO, 13751, 12766, 0, 1, CIRCULATION-LOOP, 0, HEAT-SETPT-CTRL,  0, STD, 180,  95, 110, 150, 19, 3,      "Setpoint Control:",  LEFT, -135, 5, 0, LEFT, 4, 5, "The loop temperature control sequence"
       EDIT, 13752, 12767, 0, 1, CIRCULATION-LOOP, 0,    HEAT-SETPT-T, -1, STD, 180, 120,  23,  50,  1, 3,  "Setpoint Temperature:",  LEFT, -135, 5, 1, LEFT, 4, 5, "The loop heating setpoint"
      COMBO, 13753, 12768, 0, 1, CIRCULATION-LOOP, 0,  HEAT-RESET-SCH,  0, STD, 180, 145, 200, 150, 19, 3,        "Reset Schedule:",  LEFT, -135, 5, 0, LEFT, 4, 5, "A Reset Temperature Schedule that specifies the heating setpoint"
      COMBO, 13754, 12769, 0, 1, CIRCULATION-LOOP, 0,  HEAT-SETPT-SCH,  0, STD, 180, 170, 200, 150, 19, 3,     "Setpoint Schedule:",  LEFT, -135, 5, 0, LEFT, 4, 5, "Specifies the loop heating setpoint (a Temperature Schedule)"
      COMBO, 13755, 12770, 0, 1, CIRCULATION-LOOP, 0, HEAT-EQUIP-CTRL,  0, STD, 180, 195, 200, 150, 19, 3,     "Equipment Control:",  LEFT, -135, 5, 0, LEFT, 4, 5, "An Equipment Control sequence for the primary heating equipment that serves this loop"

      LABEL, "Cooling", STD, LEFT, 380, 75, 0, 0, 1, 680, 13756, 3
      COMBO, 13756, 12771, 0, 1, CIRCULATION-LOOP, 0, COOL-SETPT-CTRL,  0, STD, 530,  95, 110, 150, 19, 3,      "Setpoint Control:",  LEFT, -135, 5, 0, LEFT, 4, 5, "The loop temperature control sequence"
       EDIT, 13757, 12772, 0, 1, CIRCULATION-LOOP, 0,    COOL-SETPT-T, -1, STD, 530, 120,  23,  50,  1, 3,  "Setpoint Temperature:",  LEFT, -135, 5, 1, LEFT, 4, 5, "The loop cooling setpoint"
      COMBO, 13758, 12773, 0, 1, CIRCULATION-LOOP, 0,  COOL-RESET-SCH,  0, STD, 530, 145, 200, 150, 19, 3,        "Reset Schedule:",  LEFT, -135, 5, 0, LEFT, 4, 5, "A Reset Temperature Schedule that specifies the cooling setpoint"
      COMBO, 13759, 12774, 0, 1, CIRCULATION-LOOP, 0,  COOL-SETPT-SCH,  0, STD, 530, 170, 200, 150, 19, 3,     "Setpoint Schedule:",  LEFT, -135, 5, 0, LEFT, 4, 5, "Specifies the loop cooling setpoint (a Temperature Schedule)"
      COMBO, 13760, 12775, 0, 1, CIRCULATION-LOOP, 0, COOL-EQUIP-CTRL,  0, STD, 530, 195, 200, 150, 19, 3,     "Equipment Control:",  LEFT, -135, 5, 0, LEFT, 4, 5, "An Equipment Control sequence for the primary cooling equipment that serves this loop"

       EDIT, 13762, 12893, 0, 1, CIRCULATION-LOOP, 0,     MAX-RESET-T, -1, STD, 140, 265,  23,  50,  1, 3,        "Max Reset Temp:",  LEFT, -110, 5, 1, LEFT, 4, 5, "The maximum allowable supply-side loop temperature (for Chilled Water or Two Pipe loops)"    
       EDIT, 13763, 12894, 0, 1, CIRCULATION-LOOP, 0,     MIN-RESET-T, -1, STD, 140, 290,  23,  50,  1, 3,        "Min Reset Temp:",  LEFT, -110, 5, 1, LEFT, 4, 5, "The minimum allowable supply-side loop temperature (for Hot Water or Two Pipe loops)"
       EDIT, 13764, 12895, 0, 1, CIRCULATION-LOOP, 0,     MAX-ALARM-T, -1, STD, 140, 315,  23,  50,  1, 3,        "Max Alarm Temp:",  LEFT, -110, 5, 1, LEFT, 4, 5, "WLHP units are turned off when the supply temperature exceeds this value"
       EDIT, 13765, 12896, 0, 1, CIRCULATION-LOOP, 0,     MIN-ALARM-T, -1, STD, 140, 340,  23,  50,  1, 3,        "Min Alarm Temp:",  LEFT, -110, 5, 1, LEFT, 4, 5, "WLHP units are turned off when the supply temperature falls below this value"

; SAC 11/30/10 - added for DOE-2.3
      LABEL, "Free Cooling", STD, LEFT, 235, 245, 0, 0, 1, 450, 19261, 3
       EDIT, 19261,     0, 0, 1, CIRCULATION-LOOP, 0,    START-WSE-WB, -1, STD, 385, 265,  23,  50,  1, 3,      "Initiate Wetbulb:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The wetbulb temperature below which free cooling is intiated"
       EDIT, 19262,     0, 0, 1, CIRCULATION-LOOP, 0,    START-WSE-DB, -1, STD, 385, 290,  23,  50,  1, 3,      "Initiate Drybulb:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The drybulb temperature below which free cooling is initiated"
       EDIT, 19263,     0, 0, 1, CIRCULATION-LOOP, 0,       WSE-SETPT, -1, STD, 385, 315,  23,  50,  1, 3, "Free Cooling Setpoint:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The condenser setpoint during free cooling"
      COMBO, 19264,     0, 0, 1, CIRCULATION-LOOP, 0,   SERIES-BYPASS, -1, STD, 385, 340, 100,  65, 19, 3,  "Bypass when inactive?",  LEFT, -140, 5, 0, LEFT, 4, 5, "Yes means water-side economizers will be bypassed when inactive"

;     LABEL, "Freeze Protection:", ITALIC_UND, LEFT, 30, 225, 0, 0, 1, 3
      LABEL, "Freeze Protection", STD, LEFT, 485, 245, 0, 0, 1, 680, 13734, 3
       EDIT, 13734, 13734, 0, 1, CIRCULATION-LOOP, 0,   RESTART-AIR-T, -1, STD, 615, 265,  23,  50,  1, 3,      "OSA Restart Temp:",  LEFT, -120, 5, 1, LEFT, 4, 5, "The temperature at (or below) which the loop restarts and runs to provide freeze protection"
       EDIT, 13735, 13735, 0, 1, CIRCULATION-LOOP, 0, RESTART-SETPT-T, -1, STD, 615, 290,  23,  50,  1, 3,    "Freeze Cycle Setpt:",  LEFT, -120, 5, 1, LEFT, 4, 5, "The heating setpoint of the loop when a WLHP restarts to avoid freezing"

; SAC 11/30/10 - added for DOE-2.3
       EDIT, 19269,     0, 0, 1, CIRCULATION-LOOP, 0,   CW-AMBIENT-DT, -1, STD, 585, 325,  23,  50,  1, 3,         "CW-Ambient dT:",  LEFT, -100, 5, 1, LEFT, 4, 5, "For WETBULB-RESET, the differential between the hourly cooling setpoint and the wetbulb"
       EDIT, 19270,     0, 0, 1, CIRCULATION-LOOP, 0,   WETBULB-RATIO, -1, STD, 585, 350,  23,  50,  2, 3,         "Wetbulb Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "For WETBULB-RESET, the ratio applied to the difference between the design wetbulb and actual wetbulb"


    ;******************************************
    ; Loop Parameters - Auxiliaries Page
    ;******************************************
    TABPAGE, 3068, 29023, 1, 3, NOTIMP, " Auxiliaries "

       EDIT, 13766, 12848, 0, 1, CIRCULATION-LOOP, 0,    LOOP-AUX-KW, -1, STD, 210, 32,  23,  50,  1, 3,       "Loop Auxiliary kW:",  LEFT, -160, 5, 1, LEFT, 4, 5, "Maximum input power required by auxiliary electrical loads on this loop"
      COMBO, 13767, 12849, 0, 1, CIRCULATION-LOOP, 0,   LOOP-AUX-SCH,  0, STD, 210, 57, 200, 140, 19, 3, "Loop Auxiliary Schedule:",  LEFT, -160, 5, 0, LEFT, 4, 5, "A fractional schedule that adjusts the Loop's Auxiliary Power "
      COMBO, 13768, 12850, 0, 1, CIRCULATION-LOOP, 0, LOOP-AUX-METER,  0, STD, 210, 82, 120, 140, 19, 3,    "Loop Auxiliary Meter:",  LEFT, -160, 5, 0, LEFT, 4, 5, "The electrical meter that tallies the Loop's Auxiliary Load"

 

 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**		Equipment Controls Tab Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
MODTABDLG, 3095, 32073, 1,  50, 100, 470, 710, 0, EQUIP-CTRL, "Equipment Control Properties", NOTIMP, 0, NOTIMP, 0 
 
    COMBO, 14018, 14018, 0, 1, EQUIP-CTRL,             0, NAME, -1, STD, 290,  15, 200, 200, 19, 3, "Currently Active Equipment Control:", RIGHT, -5, 5, 0, LEFT, 4, 5, ""	
   STATIC, 1, EQUIP-CTRL, 0, TYPE, 0, 0, 0, 515, 20, 300, STD, LEFT, "Type:  ",   "", 0, 3

   ;*****************************************
   ; General 
   ;*****************************************
    
   TABPAGE, 3096, 32073, 1, 3, NOTIMP, " General "
 
     EDIT, 14019, 14019, 0, 1, EQUIP-CTRL, 0,               NAME,  0, STD, 150,  25,  23, 180, 32, 3,  "Equip Control Name:",  LEFT, -130, 5, 0, LEFT, 4, 5, "List of all equipment control sequences defined in project; also allows library retrieval"
    COMBO, 14020, 14020, 0, 1, EQUIP-CTRL, 0,               TYPE,  0, STD, 150,  50, 300, 180, 19, 3,  "Equip Control Type:",  LEFT, -130, 5, 0, LEFT, 4, 5, "The type of load that this Equipment Control sequence applies to"
    
     CASE,  EQUIP-CTRL,  0, TYPE,  -1,  =, 1, 1
      COMBO, 19103, 19103, 0, 1, EQUIP-CTRL, 1, CIRCULATION-LOOP,  0, STD, 150,  75, 110, 180, 19, 3,    "Circulation Loop:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Name of the Loop this Equipment Control sequence applies to"
      COMBO, 19191, 19191, 0, 1, EQUIP-CTRL, 1,     PRORATE-LOAD,  0, STD, 150, 100, 110, 100, 19, 3,        "Prorate Load:",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
     ENDCASE
    
     CASE,  EQUIP-CTRL,  0, TYPE,  -1,  =, 1, 2
      COMBO, 19104, 19103, 0, 1, EQUIP-CTRL, 2, CIRCULATION-LOOP,  0, STD, 150,  75, 110, 180, 19, 3,    "Circulation Loop:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Name of the Loop this Equipment Control sequence applies to"
      COMBO, 19192, 19192, 0, 1, EQUIP-CTRL, 2,     PRORATE-LOAD,  0, STD, 150, 100, 110, 100, 19, 3,        "Prorate Load:",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
     ENDCASE
   
     CASE,  EQUIP-CTRL,  0, TYPE,  -1,  =, 1, 3
      COMBO, 19105, 19103, 0, 1, EQUIP-CTRL, 3, CIRCULATION-LOOP,  0, STD, 150,  75, 110, 180, 19, 3,    "Circulation Loop:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Name of the Loop this Equipment Control sequence applies to"
      COMBO, 19193, 19193, 0, 1, EQUIP-CTRL, 3,     PRORATE-LOAD,  0, STD, 150, 100, 110, 100, 19, 3,        "Prorate Load:",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
     ENDCASE
   
     CASE,  EQUIP-CTRL,  0, TYPE,  -1,  =, 1, 4
      COMBO, 19106, 19103, 0, 1, EQUIP-CTRL, 4, CIRCULATION-LOOP,  0, STD, 150,  75, 110, 180, 19, 3,    "Circulation Loop:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Name of the Loop this Equipment Control sequence applies to"
      COMBO, 19194, 19194, 0, 1, EQUIP-CTRL, 4,     PRORATE-LOAD,  0, STD, 150, 100, 110, 100, 19, 3,        "Prorate Load:",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
     ENDCASE
    
     CASE,  EQUIP-CTRL,  0, TYPE,  -1,  =, 1, 5
      COMBO, 14052, 14052, 0, 1, EQUIP-CTRL, 5,       ELEC-METER,  0, STD, 150,  75, 110, 180, 19, 3,      "Electric Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Name of the Electric Meter for which this control sequence controls the attached generators"
      COMBO, 19195, 19195, 0, 1, EQUIP-CTRL, 5,     PRORATE-LOAD,  0, STD, 150, 100, 110, 100, 19, 3,        "Prorate Load:",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
     ENDCASE

   ;*****************************************
   ; Load Range 1 
   ;*****************************************
   TABPAGE, 3097, 32073, 1, 3, NOTIMP, " Load Range 1 "
   
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 1
;       EDIT, 14053, 14053, 0, 1, EQUIP-CTRL, 1,     LOADS-THRU-1, 0, STD, 120,  10,  23,  70,  1, 3,     "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"	   ; SAC 11/24/10 - removed
     SPREAD, 11570, 11570, 0, 1, 0, PowerDOE, 0, EquipCtrl1Cl,    0, STD,  20,  50, 220, 315, 19, 3, "",                   LEFT,    0, 5, 0, LEFT, 0, 0, ""
     
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14025, 3
       EDIT, 14025, 14025, 0, 1, EQUIP-CTRL, 1,      STORE-SEQ-1, 0, STD, 105, 305,  23,  60,  1, 3,          "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the flow"    
       EDIT, 14026, 14026, 0, 1, EQUIP-CTRL, 1, STORE-MAX-FLOW-1, 0, STD, 105, 330,  23,  60,  1, 3,          "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"    
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14027, 3
       EDIT, 14027, 14027, 0, 1, EQUIP-CTRL, 1,      METER-SEQ-1, 0, STD, 340, 305,  23,  60,  1, 3,          "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"    
       EDIT, 14028, 14028, 0, 1, EQUIP-CTRL, 1, METER-MAX-FLOW-1, 0, STD, 340, 330,  23,  60,  1, 3,          "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 2
;       EDIT, 14054, 14053, 0, 1, EQUIP-CTRL, 2,     LOADS-THRU-1, 0, STD, 120,  10,  23,  70,  1, 3,     "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"	   ; SAC 11/24/10 - removed
      
     SPREAD, 11572, 11572, 0, 1, 0, PowerDOE, 0,    EquipCtrl1Ht, 0, STD,  20,  50, 220, 315, 19, 3,                   "", LEFT,    0, 5, 0, LEFT, 0, 0, ""
     SPREAD, 11571, 11571, 0, 1, 0, PowerDOE, 0,   EquipCtrl1Ht2, 0, STD, 365,  50, 220, 315, 19, 3,                   "", LEFT,    0, 5, 0, LEFT, 0, 0, ""
      
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14058, 3
       EDIT, 14058, 14025, 0, 1, EQUIP-CTRL, 2,      STORE-SEQ-1, 0, STD, 105, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the flow"
       EDIT, 14059, 14026, 0, 1, EQUIP-CTRL, 2, STORE-MAX-FLOW-1, 0, STD, 105, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14060, 3
       EDIT, 14060, 14027, 0, 1, EQUIP-CTRL, 2,      METER-SEQ-1, 0, STD, 340, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14061, 14028, 0, 1, EQUIP-CTRL, 2, METER-MAX-FLOW-1, 0, STD, 340, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 3
;       EDIT, 14055, 14053, 0, 1, EQUIP-CTRL, 3,     LOADS-THRU-1, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
     SPREAD, 11573, 11573, 0, 1, 0, PowerDOE, 0,  EquipCtrl1DHW,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14064, 3
       EDIT, 14064, 14027, 0, 1, EQUIP-CTRL, 3,      METER-SEQ-1, 0, STD, 340, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14065, 14028, 0, 1, EQUIP-CTRL, 3, METER-MAX-FLOW-1, 0, STD, 340, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 4
;       EDIT, 14022, 14022, 0, 1, EQUIP-CTRL, 4,     FLOWS-THRU-1, 0, STD, 120,  10,  23,  70,  1, 3, "Flows Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "Maximum flow rate for which the Heat Rejection device is used"  ; SDG 7/22/14 - removed
      
     SPREAD, 11574, 11574, 0, 1, 0, PowerDOE, 0,   EquipCtrl1HR,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     SPREAD, 11684, 11684, 0, 1, 0, PowerDOE, 0,  EquipCtrl1HR2,  0, STD, 365,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 5
;       EDIT, 14056, 14053, 0, 1, EQUIP-CTRL, 5,     LOADS-THRU-1, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
      
     SPREAD, 11575, 11575, 0, 1, 0, PowerDOE, 0,  EquipCtrl1Elec, 0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
    
     BUTTON, 10327, 10327, 0, 1, 92, 3125, STD, 505, 355, 23, 187, 3,    "Examine Load Management", "Examine Load Management"
    
   ;*****************************************
   ; Load Range 2 
   ;*****************************************
   TABPAGE, 3098, 32073, 1, 3, NOTIMP, " Load Range 2 "
 
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 1
;       EDIT, 14024, 14053, 0, 1, EQUIP-CTRL, 1,     LOADS-THRU-2, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"	   ; SAC 11/24/10 - removed
     SPREAD, 11576, 11576, 0, 1, 0, PowerDOE, 0,   EquipCtrl2Cl,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14029, 3
       EDIT, 14029, 14025, 0, 1, EQUIP-CTRL, 1,      STORE-SEQ-2, 0, STD, 105, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the load"
       EDIT, 14030, 14026, 0, 1, EQUIP-CTRL, 1, STORE-MAX-FLOW-2, 0, STD, 105, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14031, 3
       EDIT, 14031, 14027, 0, 1, EQUIP-CTRL, 1,      METER-SEQ-2, 0, STD, 340, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14032, 14028, 0, 1, EQUIP-CTRL, 1, METER-MAX-FLOW-2, 0, STD, 340, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 2
;       EDIT, 14034, 14053, 0, 1, EQUIP-CTRL, 2,     LOADS-THRU-2, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
      
     SPREAD, 11577, 11577, 0, 1, 0, PowerDOE, 0,   EquipCtrl2Ht,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     SPREAD, 11578, 11578, 0, 1, 0, PowerDOE, 0,  EquipCtrl2Ht2,  0, STD, 365,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14035, 3
       EDIT, 14035, 14025, 0, 1, EQUIP-CTRL, 2,      STORE-SEQ-2, 0, STD, 105, 305,  23,  60,  1, 3,        "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the flow"
       EDIT, 14036, 14026, 0, 1, EQUIP-CTRL, 2, STORE-MAX-FLOW-2, 0, STD, 105, 330,  23,  60,  1, 3,        "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14037, 3
       EDIT, 14037, 14027, 0, 1, EQUIP-CTRL, 2,      METER-SEQ-2, 0, STD, 340, 305,  23,  60,  1, 3,        "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14039, 14028, 0, 1, EQUIP-CTRL, 2, METER-MAX-FLOW-2, 0, STD, 340, 330,  23,  60,  1, 3,        "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 3
;       EDIT, 14040, 14053, 0, 1, EQUIP-CTRL, 3,     LOADS-THRU-2, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
     SPREAD, 11579, 11579, 0, 1, 0, PowerDOE, 0,  EquipCtrl2DHW,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
                                                                          
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14041, 3       
       EDIT, 14041, 14027, 0, 1, EQUIP-CTRL, 3,      METER-SEQ-2, 0, STD, 340, 305,  23,  60,  1, 3, "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14042, 14028, 0, 1, EQUIP-CTRL, 3, METER-MAX-FLOW-2, 0, STD, 340, 330,  23,  60,  1, 3, "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 4
;       EDIT, 14044, 14022, 0, 1, EQUIP-CTRL, 4,     FLOWS-THRU-2, 0, STD, 120,  10,  23,  70,  1, 3, "Flows Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "Maximum flow rate for which the Heat Rejection device is used" ; SDG 7/22/14 - removed
      
     SPREAD, 11580, 11580, 0, 1, 0, PowerDOE, 0,   EquipCtrl2HR,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     SPREAD, 11685, 11685, 0, 1, 0, PowerDOE, 0,  EquipCtrl2HR2,  0, STD, 365,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 5
;       EDIT, 14045, 14053, 0, 1, EQUIP-CTRL, 5,     LOADS-THRU-2, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, 100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
      
     SPREAD, 11581, 11581, 0, 1, 0, PowerDOE, 0,  EquipCtrl2Elec, 0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
 
     BUTTON, 10332, 10332, 0, 1, 92, 3125, STD, 505, 355, 23, 187, 3,    "Examine Load Management", "Examine Load Management"
 
   ;*****************************************
   ; Load Range 3 
   ;*****************************************
   TABPAGE, 3099, 32073, 1, 3, NOTIMP, " Load Range 3 "
 
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 1
;       EDIT, 14046, 14053, 0, 1, EQUIP-CTRL, 1,     LOADS-THRU-3, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
     SPREAD, 11582, 11582, 0, 1, 0, PowerDOE, 0,   EquipCtrl3Cl,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14047, 3
       EDIT, 14047, 14025, 0, 1, EQUIP-CTRL, 1,      STORE-SEQ-3, 0, STD, 105, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the flow"
       EDIT, 14057, 14026, 0, 1, EQUIP-CTRL, 1, STORE-MAX-FLOW-3, 0, STD, 105, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14062, 3
       EDIT, 14062, 14027, 0, 1, EQUIP-CTRL, 1,      METER-SEQ-3, 0, STD, 340, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14063, 14028, 0, 1, EQUIP-CTRL, 1, METER-MAX-FLOW-3, 0, STD, 340, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 2
;       EDIT, 14066, 14053, 0, 1, EQUIP-CTRL, 2,     LOADS-THRU-3, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
      
     SPREAD, 11583, 11583, 0, 1, 0, PowerDOE, 0,   EquipCtrl3Ht,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     SPREAD, 11584, 11584, 0, 1, 0, PowerDOE, 0,  EquipCtrl3Ht2,  0, STD, 365,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14067, 3
       EDIT, 14067, 14025, 0, 1, EQUIP-CTRL, 2,      STORE-SEQ-3, 0, STD, 105, 305,  23,  60,  1, 3,        "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the flow"
       EDIT, 14068, 14026, 0, 1, EQUIP-CTRL, 2, STORE-MAX-FLOW-3, 0, STD, 105, 330,  23,  60,  1, 3,        "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14069, 3
       EDIT, 14069, 14027, 0, 1, EQUIP-CTRL, 2,      METER-SEQ-3, 0, STD, 340, 305,  23,  60,  1, 3,        "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14070, 14028, 0, 1, EQUIP-CTRL, 2, METER-MAX-FLOW-3, 0, STD, 340, 330,  23,  60,  1, 3,        "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE

    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 3
;       EDIT, 14071, 14053, 0, 1, EQUIP-CTRL, 3,     LOADS-THRU-3, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
     SPREAD, 11585, 11585, 0, 1, 0, PowerDOE, 0,  EquipCtrl3DHW,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14041, 3       
       EDIT, 14072, 14027, 0, 1, EQUIP-CTRL, 3,      METER-SEQ-3, 0, STD, 340, 305,  23,  60,  1, 3, "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14073, 14028, 0, 1, EQUIP-CTRL, 3, METER-MAX-FLOW-3, 0, STD, 340, 330,  23,  60,  1, 3, "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 4
;       EDIT, 14074, 14022, 0, 1, EQUIP-CTRL, 4,     FLOWS-THRU-3, 0, STD, 120,  10,  23,  70,  1, 3, "Flows Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "Maximum flow rate for which the Heat Rejection device is used" ; SDG 7/22/14 - removed
      
     SPREAD, 11586, 11586, 0, 1, 0, PowerDOE, 0,   EquipCtrl3HR,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     SPREAD, 11686, 11686, 0, 1, 0, PowerDOE, 0,  EquipCtrl3HR2,  0, STD, 365,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 5
;       EDIT, 14075, 14053, 0, 1, EQUIP-CTRL, 5,     LOADS-THRU-3, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
      
     SPREAD, 11587, 11587, 0, 1, 0, PowerDOE, 0,  EquipCtrl3Elec, 0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
 
     BUTTON, 10333, 10333, 0, 1, 92, 3125, STD, 505, 355, 23, 187, 3,    "Examine Load Management", "Examine Load Management"
 
   ;*****************************************
   ; Load Range 4
   ;*****************************************
   TABPAGE, 3100, 32073, 1, 3, NOTIMP, " Load Range 4 "
 
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 1
;       EDIT, 14076, 14053, 0, 1, EQUIP-CTRL, 1,     LOADS-THRU-4, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
     SPREAD, 11588, 11588, 0, 1, 0, PowerDOE, 0,   EquipCtrl4Cl,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14077, 3
       EDIT, 14077, 14025, 0, 1, EQUIP-CTRL, 1,      STORE-SEQ-4, 0, STD, 105, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the flow"
       EDIT, 14078, 14026, 0, 1, EQUIP-CTRL, 1, STORE-MAX-FLOW-4, 0, STD, 105, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14079, 3
       EDIT, 14079, 14027, 0, 1, EQUIP-CTRL, 1,      METER-SEQ-4, 0, STD, 340, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14080, 14028, 0, 1, EQUIP-CTRL, 1, METER-MAX-FLOW-4, 0, STD, 340, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 2
;       EDIT, 14081, 14053, 0, 1, EQUIP-CTRL, 2,     LOADS-THRU-4, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed

     SPREAD, 11589, 11589, 0, 1, 0, PowerDOE, 0,   EquipCtrl4Ht,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     SPREAD, 11590, 11590, 0, 1, 0, PowerDOE, 0,  EquipCtrl4Ht2,  0, STD, 365,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14082, 3
       EDIT, 14082, 14025, 0, 1, EQUIP-CTRL, 2,      STORE-SEQ-4, 0, STD, 105, 305,  23,  60,  1, 3,        "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the flow"
       EDIT, 14083, 14026, 0, 1, EQUIP-CTRL, 2, STORE-MAX-FLOW-4, 0, STD, 105, 330,  23,  60,  1, 3,        "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14084, 3
       EDIT, 14084, 14027, 0, 1, EQUIP-CTRL, 2,      METER-SEQ-4, 0, STD, 340, 305,  23,  60,  1, 3,        "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14085, 14028, 0, 1, EQUIP-CTRL, 2, METER-MAX-FLOW-4, 0, STD, 340, 330,  23,  60,  1, 3,        "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE

    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 3
;       EDIT, 14086, 14053, 0, 1, EQUIP-CTRL, 3,     LOADS-THRU-4, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
     SPREAD, 11591, 11591, 0, 1, 0, PowerDOE, 0,  EquipCtrl4DHW,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""

      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14087, 3
       EDIT, 14087, 14027, 0, 1, EQUIP-CTRL, 3,      METER-SEQ-4, 0, STD, 340, 305,  23,  60,  1, 3, "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14088, 14028, 0, 1, EQUIP-CTRL, 3, METER-MAX-FLOW-4, 0, STD, 340, 330,  23,  60,  1, 3, "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 4
;       EDIT, 14089, 14022, 0, 1, EQUIP-CTRL, 4,     FLOWS-THRU-4, 0, STD, 120,  10,  23,  70,  1, 3, "Flows Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "Maximum flow rate for which the Heat Rejection device is used" ; SDG 7/22/14 - removed
      
     SPREAD, 11592, 11592, 0, 1, 0, PowerDOE, 0,   EquipCtrl4HR,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     SPREAD, 11687, 11687, 0, 1, 0, PowerDOE, 0,  EquipCtrl4HR2,  0, STD, 365,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE

    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 5
;       EDIT, 14090, 14053, 0, 1, EQUIP-CTRL, 5,     LOADS-THRU-4, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
      
     SPREAD, 11593, 11593, 0, 1, 0, PowerDOE, 0,  EquipCtrl4Elec, 0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
 
     BUTTON, 10344, 10344, 0, 1, 92, 3125, STD, 505, 355, 23, 187, 3,    "Examine Load Management", "Examine Load Management"

   ;*****************************************
   ; Load Range 5
   ;*****************************************
   TABPAGE, 3101, 32073, 1, 3, NOTIMP, " Load Range 5 "
 
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 1
;       EDIT, 14091, 14053, 0, 1, EQUIP-CTRL, 1,     LOADS-THRU-5, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
     SPREAD, 11594, 11594, 0, 1, 0, PowerDOE, 0,   EquipCtrl5Cl,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14092, 3
       EDIT, 14092, 14025, 0, 1, EQUIP-CTRL, 1,      STORE-SEQ-5, 0, STD, 105, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the flow"
       EDIT, 14093, 14026, 0, 1, EQUIP-CTRL, 1, STORE-MAX-FLOW-5, 0, STD, 105, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14094, 3
       EDIT, 14094, 14027, 0, 1, EQUIP-CTRL, 1,      METER-SEQ-5, 0, STD, 340, 305,  23,  60,  1, 3,         "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14095, 14028, 0, 1, EQUIP-CTRL, 1, METER-MAX-FLOW-5, 0, STD, 340, 330,  23,  60,  1, 3,         "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 2
;       EDIT, 14096, 14053, 0, 1, EQUIP-CTRL, 2,     LOADS-THRU-5, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
      
     SPREAD, 11595, 11595, 0, 1, 0, PowerDOE, 0,   EquipCtrl5Ht,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     SPREAD, 11596, 11596, 0, 1, 0, PowerDOE, 0,  EquipCtrl5Ht2,  0, STD, 365,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      
      LABEL, "Storage", STD, LEFT,  20, 290, 0, 0, 1, 205, 14097, 3
       EDIT, 14097, 14025, 0, 1, EQUIP-CTRL, 2,      STORE-SEQ-5, 0, STD, 105, 305,  23,  60,  1, 3,        "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the thermal storage device is used to satisfy the flow"
       EDIT, 14098, 14026, 0, 1, EQUIP-CTRL, 2, STORE-MAX-FLOW-5, 0, STD, 105, 330,  23,  60,  1, 3,        "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the thermal storage device"
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14099, 3
       EDIT, 14099, 14027, 0, 1, EQUIP-CTRL, 2,      METER-SEQ-5, 0, STD, 340, 305,  23,  60,  1, 3,        "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14100, 14028, 0, 1, EQUIP-CTRL, 2, METER-MAX-FLOW-5, 0, STD, 340, 330,  23,  60,  1, 3,        "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE

    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 3
;       EDIT, 14101, 14053, 0, 1, EQUIP-CTRL, 3,     LOADS-THRU-5, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
     SPREAD, 11597, 11597, 0, 1, 0, PowerDOE, 0,  EquipCtrl5DHW,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      
      LABEL, "Meter", STD, LEFT,   255, 290, 0, 0, 1, 440, 14102, 3
       EDIT, 14102, 14027, 0, 1, EQUIP-CTRL, 3,      METER-SEQ-5, 0, STD, 340, 305,  23,  60,  1, 3, "Sequence:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The order in which the meter is used to satisfy the flow"
       EDIT, 14103, 14028, 0, 1, EQUIP-CTRL, 3, METER-MAX-FLOW-5, 0, STD, 340, 330,  23,  60,  1, 3, "Max Flow:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "The maximum allowable flow for the meter"
    ENDCASE
    
    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 4
;       EDIT, 14104, 14022, 0, 1, EQUIP-CTRL, 4,     FLOWS-THRU-5, 0, STD, 120,  10,  23,  70,  1, 3, "Flows Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "Maximum flow rate for which the Heat Rejection device is used" ; SDG 7/22/14 - removed
      
     SPREAD, 11598, 11598, 0, 1, 0, PowerDOE, 0,   EquipCtrl5HR,  0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     SPREAD, 11688, 11688, 0, 1, 0, PowerDOE, 0,  EquipCtrl5HR2,  0, STD, 365,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE

    CASE, EQUIP-CTRL, 0, TYPE, -1, =, 1, 5
;       EDIT, 14105, 14053, 0, 1, EQUIP-CTRL, 5,     LOADS-THRU-5, 0, STD, 120,  10,  23,  70,  1, 3, "Loads Through:", LEFT, -100, 5, 1, LEFT, 4, 5, "The load threshold up to which the corresponding piece of equipment is used to satisfy"   ; SAC 11/24/10 - removed
      
     SPREAD, 11599, 11599, 0, 1, 0, PowerDOE, 0,  EquipCtrl5Elec, 0, STD,  20,  50, 220, 315, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
 
     BUTTON, 10346, 10346, 0, 1, 92, 3125, STD, 505, 355, 23, 187, 3,    "Examine Load Management", "Examine Load Management"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**		Load Management Tab Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODTABDLG, 3124, 32073, 1,  50, 100, 470, 710, 0, LOAD-MANAGEMENT, "Load Management Data: ", LOAD-MANAGEMENT, 0, NAME, 0, 0, 0, "", NOTIMP, 0, NOTIMP, 0 
MODTABDLG, 3124, 32073, 1,  50, 100, 470, 710, 0, LOAD-MANAGEMENT, "Load Management Properties", NOTIMP, 0, NOTIMP, 0 
 
    COMBO, 14285, 14285, 0, 1, LOAD-MANAGEMENT,        0, NAME, -1, STD, 280,  15, 200, 200, 19, 3, "Currently Active Load Management:", RIGHT, -5, 5, 0, LEFT, 225,  73, ""
   STATIC, 1, LOAD-MANAGEMENT, 0, TYPE, 0, 0, 0, 505, 20, 300, STD, LEFT, "Type:  ",   "", 0, 3

   ;*****************************************
   ; General 
   ;*****************************************
   TABPAGE, 3125, 32073, 1, 3, NOTIMP, " General "
 
     EDIT, 14286, 14286, 0, 1, LOAD-MANAGEMENT, 0,             NAME,  0, STD, 195,  25,  23, 250, 32, 3,        "Load Management Name:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Name of this load management sequence component"
    COMBO, 14287, 14287, 0, 1, LOAD-MANAGEMENT, 0,             TYPE,  0, STD, 195,  50, 300, 250, 19, 3,        "Load Management Type:",  LEFT, -175, 5, 0, LEFT, 4, 5, "The type of control this sequence uses"

    COMBO, 14288, 14288, 0, 1, LOAD-MANAGEMENT, 0,         QUAL-SCH,  0, STD, 195,  75, 250, 250, 19, 3,      "Qualification Schedule:",  LEFT, -175, 5, 0, LEFT, 4, 5, "A Flag schedule that defines when this Load Management sequence is active"
     EDIT, 14289, 14289, 0, 1, LOAD-MANAGEMENT, 0,    QUAL-SCH-FLAG,  0, STD, 195, 100,  23,  50,  1, 3, "Qualification Schedule Flag:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Value of the flag in the Qualification Schedule: specifies when this Load Mgmt is active"
    
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 1
;      LABEL, "Load Management Type = Scheduled:", ITALIC_UND, LEFT, 20, 162, 1, 0, 0, 3
      COMBO, 14290, 14290, 0, 1, LOAD-MANAGEMENT, 1, EQUIP-CTRL-SCH,  0, STD, 195, 125, 250, 250, 19, 3,  "Equipment Control Schedule:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Schedule with flags that switch Equipment Control sequences and/or enable/disable loops"
    ENDCASE
 
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 3
;      LABEL, "Load Management Type = Zone Temperature:", ITALIC_UND, LEFT, 20, 162, 1, 0, 0, 3
      COMBO, 14291, 14291, 0, 1, LOAD-MANAGEMENT, 3,      CTRL-ZONE,  0, STD, 195, 125, 250, 250, 19, 3,                "Control Zone:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Name of the Zone whose temperature is used to switch Equipment Control sequences"
    ENDCASE
 
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 4
;      LABEL, "Load Management Type = Loop Load:", ITALIC_UND, LEFT, 20, 162, 1, 0, 0, 3
      COMBO, 14292, 14292, 0, 1, LOAD-MANAGEMENT, 4,      CTRL-LOOP,  0, STD, 195, 125, 250, 250, 19, 3,                "Control Loop:",  LEFT, -175, 5, 0, LEFT, 4, 5, "Name of loop whose load is used to switch Equip Ctrl sequences that apply to another loop"
    ENDCASE
 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;
; CONVERSION STEPS:
;
; 1. Add BDL Command Edited (or NOTIMP) before Caption for dialogs, tabbed dialogs & tabbed dialog pages
;
; 2. Change tabbed dialog size from "310, 610" to "470, 710"
;
; 3. Change label and units label coordinates to be in relation to top-left and top-right corners of the control
;
; 4. Add two properties to each LABEL -> right shadowline X coord & ID of associated UI control (both 0 for none)
;    - also remove trailing ':'s from labels with shadowline extensions
;
; 5. Switch all ComboBox "Height of edit portion of control" values from 21 to 19
;
; 6. Switch all Edit "Height" values from 21 to 23
;
; 7. Switch all font settings of "ITALIC_UND" to "STD"
;
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
   ;*****************************************
   ; Load Management Seq  1 
   ;*****************************************
   TABPAGE, 3126, 32073, 1, 3, NOTIMP, " Managemnt Seq 1 "
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 1
      EDIT, 14294, 14294, 0, 1, LOAD-MANAGEMENT, 1,     CTRL-FLAG-1,  0, STD, 150,  15,  21,  60,  1, 3, "Equip Ctrl Sch Flag:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Flag value corresponding to one of the flag values in the Equipment Control Schedule"
      EDIT, 14366, 14366, 0, 1, LOAD-MANAGEMENT, 1, CTRL-PRIORITY-1,  0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
        
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3

      SPREAD, 11516, 11516, 0, 1, 0, PowerDOE, 0, LdMgmt1EquipCtrl1,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11617, 11617, 0, 1, 0, PowerDOE, 0,   LdMgmt1LoopsOn1,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11618, 11618, 0, 1, 0, PowerDOE, 0,  LdMgmt1LoopsOff1,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 2
      EDIT, 14295, 14295, 0, 1, LOAD-MANAGEMENT, 2,    TEMPS-THRU-1,  0, STD, 150,  15,  21,  60,  1, 3,        "Max OSA Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
      EDIT, 14367, 14366, 0, 1, LOAD-MANAGEMENT, 2, CTRL-PRIORITY-1,  0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
        
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
        
      SPREAD, 11619, 11619, 0, 1, 0, PowerDOE, 0, LdMgmt1EquipCtrl2,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11620, 11620, 0, 1, 0, PowerDOE, 0,   LdMgmt1LoopsOn2,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11621, 11621, 0, 1, 0, PowerDOE, 0,  LdMgmt1LoopsOff2,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 3
      EDIT, 14296, 14295, 0, 1, LOAD-MANAGEMENT, 3,    TEMPS-THRU-1,  0, STD, 150,  15,  21,  60,  1, 3,       "Max Zone Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
      EDIT, 14385, 14366, 0, 1, LOAD-MANAGEMENT, 3, CTRL-PRIORITY-1,  0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
        
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
        
      SPREAD, 11622, 11622, 0, 1, 0, PowerDOE, 0, LdMgmt1EquipCtrl3,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11623, 11623, 0, 1, 0, PowerDOE, 0,   LdMgmt1LoopsOn3,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11624, 11624, 0, 1, 0, PowerDOE, 0,  LdMgmt1LoopsOff3,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 4
     EDIT, 14297, 14297, 0, 1, LOAD-MANAGEMENT, 4,    LOADS-THRU-1,   0, STD, 150,  15,  21,  60,  1, 3,       "Loads Through:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum load for which this management sequence applies"
     EDIT, 14368, 14366, 0, 1, LOAD-MANAGEMENT, 4, CTRL-PRIORITY-1,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
      SPREAD, 11625, 11625, 0, 1, 0, PowerDOE, 0, LdMgmt1EquipCtrl4,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
     BUTTON, 10316, 10316, 0, 1, 92, 3096, STD, 505, 355, 23, 187, 3,    "Examine Equipment Control", "Examine Equipment Control"
   
   ;*****************************************
   ; Load Management Seq 2 
   ;*****************************************
   TABPAGE, 3127, 32073, 1, 3, NOTIMP, " Managemnt Seq 2 "
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 1
     EDIT, 14346, 14294, 0, 1, LOAD-MANAGEMENT, 1,     CTRL-FLAG-2,   0, STD, 150,  15,  21,  60,  1, 3, "Equip Ctrl Sch Flag:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Flag value corresponding to one of the flag values in the Equipment Control Schedule"
     EDIT, 14369, 14366, 0, 1, LOAD-MANAGEMENT, 1, CTRL-PRIORITY-2,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
        
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
        
      SPREAD, 11626, 11626, 0, 1, 0, PowerDOE, 0, LdMgmt2EquipCtrl1,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11627, 11627, 0, 1, 0, PowerDOE, 0,   LdMgmt2LoopsOn1,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11628, 11628, 0, 1, 0, PowerDOE, 0,  LdMgmt2LoopsOff1,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 2
     EDIT, 14347, 14295, 0, 1, LOAD-MANAGEMENT, 2,    TEMPS-THRU-2,   0, STD, 150,  15,  21,  60,  1, 3,        "Max OSA Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
     EDIT, 14370, 14366, 0, 1, LOAD-MANAGEMENT, 2, CTRL-PRIORITY-2,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11629, 11626, 0, 1, 0, PowerDOE, 0, LdMgmt2EquipCtrl2,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11630, 11627, 0, 1, 0, PowerDOE, 0,   LdMgmt2LoopsOn2,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11631, 11628, 0, 1, 0, PowerDOE, 0,  LdMgmt2LoopsOff2,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 3
     EDIT, 14348, 14295, 0, 1, LOAD-MANAGEMENT, 3,    TEMPS-THRU-2,   0, STD, 150,  15,  21,  60,  1, 3,       "Max Zone Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
     EDIT, 14371, 14366, 0, 1, LOAD-MANAGEMENT, 3, CTRL-PRIORITY-2,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11632, 11626, 0, 1, 0, PowerDOE, 0, LdMgmt2EquipCtrl3,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11633, 11627, 0, 1, 0, PowerDOE, 0,   LdMgmt2LoopsOn3,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11634, 11628, 0, 1, 0, PowerDOE, 0,  LdMgmt2LoopsOff3,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 4
     EDIT, 14349, 14297, 0, 1, LOAD-MANAGEMENT, 4,    LOADS-THRU-2,   0, STD, 150,  15,  21,  60,  1, 3,       "Loads Through:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum load for which this management sequence applies"
     EDIT, 14372, 14366, 0, 1, LOAD-MANAGEMENT, 4, CTRL-PRIORITY-2,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
      SPREAD, 11635, 11626, 0, 1, 0, PowerDOE, 0, LdMgmt2EquipCtrl4,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
     BUTTON, 10317, 10317, 0, 1, 92, 3096, STD, 505, 355, 23, 187, 3,    "Examine Equipment Control", "Examine Equipment Control"
   
   ;*****************************************
   ; Load Manaagement Seq  3 
   ;*****************************************
   TABPAGE, 3128, 32073, 1, 3, NOTIMP, " Managemnt Seq 3 "
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 1
     EDIT, 14351, 14294, 0, 1, LOAD-MANAGEMENT, 1,    CTRL-FLAG-3,    0, STD, 150,  15,  21,  60,  1, 3, "Equip Ctrl Sch Flag:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Flag value corresponding to one of the flag values in the Equipment Control Schedule"
     EDIT, 14373, 14366, 0, 1, LOAD-MANAGEMENT, 1, CTRL-PRIORITY-3,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11636, 11636, 0, 1, 0, PowerDOE, 0, LdMgmt3EquipCtrl1,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11637, 11637, 0, 1, 0, PowerDOE, 0,   LdMgmt3LoopsOn1,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11638, 11638, 0, 1, 0, PowerDOE, 0,  LdMgmt3LoopsOff1,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 2
     EDIT, 14352, 14295, 0, 1, LOAD-MANAGEMENT, 2,    TEMPS-THRU-3,   0, STD, 150,  15,  21,  60,  1, 3,        "Max OSA Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
     EDIT, 14374, 14366, 0, 1, LOAD-MANAGEMENT, 2, CTRL-PRIORITY-3,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11639, 11639, 0, 1, 0, PowerDOE, 0, LdMgmt3EquipCtrl2,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11640, 11640, 0, 1, 0, PowerDOE, 0,   LdMgmt3LoopsOn2,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11641, 11641, 0, 1, 0, PowerDOE, 0,  LdMgmt3LoopsOff2,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 3
     EDIT, 14353, 14295, 0, 1, LOAD-MANAGEMENT, 3,    TEMPS-THRU-3,   0, STD, 150,  15,  21,  60,  1, 3,       "Max Zone Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
     EDIT, 14375, 14366, 0, 1, LOAD-MANAGEMENT, 3, CTRL-PRIORITY-3,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11642, 11642, 0, 1, 0, PowerDOE, 0, LdMgmt3EquipCtrl3,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11643, 11643, 0, 1, 0, PowerDOE, 0,   LdMgmt3LoopsOn3,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11644, 11644, 0, 1, 0, PowerDOE, 0,  LdMgmt3LoopsOff3,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 4
     EDIT, 14354, 14297, 0, 1, LOAD-MANAGEMENT, 4,    LOADS-THRU-3,   0, STD, 150,  15,  21,  60,  1, 3,       "Loads Through:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum load for which this management sequence applies"
     EDIT, 14376, 14366, 0, 1, LOAD-MANAGEMENT, 4, CTRL-PRIORITY-3,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
      SPREAD, 11645, 11645, 0, 1, 0, PowerDOE, 0, LdMgmt3EquipCtrl4,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
     BUTTON, 10318, 10318, 0, 1, 92, 3096, STD, 505, 355, 23, 187, 3,    "Examine Equipment Control", "Examine Equipment Control"
   
   ;*****************************************
   ; Load Management Seq  4 
   ;*****************************************
   TABPAGE, 3129, 32073, 1, 3, NOTIMP, " Managemnt Seq 4 "
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 1
     EDIT, 14356, 14294, 0, 1, LOAD-MANAGEMENT, 1,     CTRL-FLAG-4,   0, STD, 150,  15,  21,  60,  1, 3, "Equip Ctrl Sch Flag:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Flag value corresponding to one of the flag values in the Equipment Control Schedule"
     EDIT, 14377, 14366, 0, 1, LOAD-MANAGEMENT, 1, CTRL-PRIORITY-4,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11646, 11646, 0, 1, 0, PowerDOE, 0, LdMgmt4EquipCtrl1,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11647, 11647, 0, 1, 0, PowerDOE, 0,   LdMgmt4LoopsOn1,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11648, 11648, 0, 1, 0, PowerDOE, 0,  LdMgmt4LoopsOff1,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 2
     EDIT, 14357, 14295, 0, 1, LOAD-MANAGEMENT, 2,    TEMPS-THRU-4,   0, STD, 150,  15,  21,  60,  1, 3,        "Max OSA Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
     EDIT, 14378, 14366, 0, 1, LOAD-MANAGEMENT, 2, CTRL-PRIORITY-4,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11649, 11649, 0, 1, 0, PowerDOE, 0, LdMgmt4EquipCtrl2,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11650, 11650, 0, 1, 0, PowerDOE, 0,   LdMgmt4LoopsOn2,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11651, 11651, 0, 1, 0, PowerDOE, 0,  LdMgmt4LoopsOff2,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 3
     EDIT, 14358, 14295, 0, 1, LOAD-MANAGEMENT, 3,    TEMPS-THRU-4,   0, STD, 150,  15,  21,  60,  1, 3,       "Max Zone Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
     EDIT, 14379, 14366, 0, 1, LOAD-MANAGEMENT, 3, CTRL-PRIORITY-4,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11652, 11652, 0, 1, 0, PowerDOE, 0, LdMgmt4EquipCtrl3,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11653, 11653, 0, 1, 0, PowerDOE, 0,   LdMgmt4LoopsOn3,  0, STD, 247,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11654, 11654, 0, 1, 0, PowerDOE, 0,  LdMgmt4LoopsOff3,  0, STD, 474,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 4
     EDIT, 14359, 14297, 0, 1, LOAD-MANAGEMENT, 4,    LOADS-THRU-4,   0, STD, 150,  15,  21,  60,  1, 3,       "Loads Through:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum load for which this management sequence applies"
     EDIT, 14380, 14366, 0, 1, LOAD-MANAGEMENT, 4, CTRL-PRIORITY-4,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
      SPREAD, 11655, 11655, 0, 1, 0, PowerDOE, 0, LdMgmt4EquipCtrl4,  0, STD,  20,  75, 260, 205, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
     BUTTON, 10319, 10319, 0, 1, 92, 3096, STD, 505, 355, 23, 187, 3,    "Examine Equipment Control", "Examine Equipment Control"
   
   ;*****************************************
   ; Load Management Seq  5 
   ;*****************************************
   TABPAGE, 3130, 32073, 1, 3, NOTIMP, " Managemnt Seq 5 "
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 1
     EDIT, 14361, 14294, 0, 1, LOAD-MANAGEMENT, 1,    CTRL-FLAG-5,    0, STD, 150,  15,  21,  60,  1, 3, "Equip Ctrl Sch Flag:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Flag value corresponding to one of the flag values in the Equipment Control Schedule"
     EDIT, 14381, 14366, 0, 1, LOAD-MANAGEMENT, 1, CTRL-PRIORITY-5,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11656, 11656, 0, 1, 0, PowerDOE, 0, LdMgmt5EquipCtrl1,  0, STD,  20,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11657, 11657, 0, 1, 0, PowerDOE, 0,   LdMgmt5LoopsOn1,  0, STD, 247,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11658, 11658, 0, 1, 0, PowerDOE, 0,  LdMgmt5LoopsOff1,  0, STD, 474,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 2
     EDIT, 14362, 14295, 0, 1, LOAD-MANAGEMENT, 2,    TEMPS-THRU-5,   0, STD, 150,  15,  21,  60,  1, 3,        "Max OSA Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
     EDIT, 14382, 14366, 0, 1, LOAD-MANAGEMENT, 2, CTRL-PRIORITY-5,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11659, 11659, 0, 1, 0, PowerDOE, 0, LdMgmt5EquipCtrl2,  0, STD,  20,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11660, 11660, 0, 1, 0, PowerDOE, 0,   LdMgmt5LoopsOn2,  0, STD, 247,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11661, 11661, 0, 1, 0, PowerDOE, 0,  LdMgmt5LoopsOff2,  0, STD, 474,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 3
     EDIT, 14363, 14295, 0, 1, LOAD-MANAGEMENT, 3,    TEMPS-THRU-5,   0, STD, 150,  15,  21,  60,  1, 3,       "Max Zone Temp:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum temperature for which this management sequence applies"
     EDIT, 14383, 14366, 0, 1, LOAD-MANAGEMENT, 3, CTRL-PRIORITY-5,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
     
       LABEL,   "Loops forced ON or OFF by a schedule flag or maximum", STD, LEFT, 290, 20, 1, 0, 0, 0, 0, 3
       LABEL, "temperature condition specified for this Control Range", STD, LEFT, 290, 37, 1, 0, 0, 0, 0, 3
     
      SPREAD, 11662, 11662, 0, 1, 0, PowerDOE, 0, LdMgmt5EquipCtrl3,  0, STD,  20,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11663, 11663, 0, 1, 0, PowerDOE, 0,   LdMgmt5LoopsOn3,  0, STD, 247,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
      SPREAD, 11664, 11664, 0, 1, 0, PowerDOE, 0,  LdMgmt5LoopsOff3,  0, STD, 474,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
    CASE, LOAD-MANAGEMENT, 0, TYPE, -1, =, 1, 4
     EDIT, 14364, 14297, 0, 1, LOAD-MANAGEMENT, 4,    LOADS-THRU-5,   0, STD, 150,  15,  21,  60,  1, 3,       "Loads Through:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The maximum load for which this management sequence applies"
     EDIT, 14384, 14366, 0, 1, LOAD-MANAGEMENT, 4, CTRL-PRIORITY-5,   0, STD, 150,  40,  21,  60,  1, 3,            "Priority:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The Equipment Ctrl sequence with highest priority overrides all others when a conflict exists"
      SPREAD, 11665, 11665, 0, 1, 0, PowerDOE, 0, LdMgmt5EquipCtrl4,  0, STD,  20,  75, 260, 205, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
    ENDCASE
   
     BUTTON, 10320, 10320, 0, 1, 92, 3096, STD, 505, 355, 23, 187, 3,    "Examine Equipment Control", "Examine Equipment Control"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Chiller - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; CHILLER:TYPE as of v41 (~9/2002) 
;      1> TYPE                                Symbolic Defined    1  250 (CODE-WORD       )  TABLE =0    1         -9 (* Required *    )
;                                  SYMBOL TABLE ENTRY   ELEC-OPEN-CENT                   TYPE =  250 DEF/REF  -1/ -1      VALUE =    1
;                                  SYMBOL TABLE ENTRY   ELEC-OPEN-REC                    TYPE =  250 DEF/REF  -1/ -1      VALUE =    2
;                                  SYMBOL TABLE ENTRY   ELEC-HERM-CENT                   TYPE =  250 DEF/REF  -1/ -1      VALUE =    3
;                                  SYMBOL TABLE ENTRY   ELEC-HERM-REC                    TYPE =  250 DEF/REF  -1/ -1      VALUE =    4
;                                  SYMBOL TABLE ENTRY   ELEC-SCREW                       TYPE =  250 DEF/REF  -1/ -1      VALUE =   12
;                                  SYMBOL TABLE ENTRY   ELEC-HTREC                       TYPE =  250 DEF/REF  -1/ -1      VALUE =    5
;                                  SYMBOL TABLE ENTRY   ABSOR-1                          TYPE =  250 DEF/REF  -1/ -1      VALUE =    6
;                                  SYMBOL TABLE ENTRY   ABSOR-2                          TYPE =  250 DEF/REF  -1/ -1      VALUE =    7
;                                  SYMBOL TABLE ENTRY   GAS-ABSOR                        TYPE =  250 DEF/REF  -1/ -1      VALUE =    8
;                                  SYMBOL TABLE ENTRY   ENGINE                           TYPE =  250 DEF/REF  -1/ -1      VALUE =    9
;                                  SYMBOL TABLE ENTRY   HEAT-PUMP                        TYPE =  250 DEF/REF  -1/ -1      VALUE =   10
;                                  SYMBOL TABLE ENTRY   LOOP-TO-LOOP-HP                  TYPE =  250 DEF/REF  -1/ -1      VALUE =   11
;                                  SYMBOL TABLE ENTRY   WATER-ECONOMIZER                 TYPE =  250 DEF/REF  -1/ -1      VALUE =   13

; MODTABDLG, 3037, 3037, 1, 100, 100, 310, 610, 0, "Chiller Type:  ", CHILLER, 0, TYPE, 0, 0, 0, "     Chiller Name:  ", CHILLER, 0, NAME, 0, 0, 0, ""
MODTABDLG, 3037, 3037, 1, 100, 100, 500, 760, 0, CHILLER, "Chiller Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 12872, 12872, 0, 1, CHILLER, 0, NAME,  0, STD, 195,  15, 400, 250, 19, 3, "Currently Active Chiller:", RIGHT, -8, 5, 0, LEFT, 4, 5, "List of all chillers defined in project; also allows library retrieval and creation"
   STATIC, 1, CHILLER, 0, TYPE, 0, 0, 0, 465, 20, 300, STD, LEFT, "Type: ",   "", 0, 3

    ;******************************************
    ; Chiller - Basic Specifications Page
    ;******************************************
    TABPAGE, 3038, 3038, 1, 3, NOTIMP, " Basic Specifications "

    EDIT, 12899, 12899, 0, 1, CHILLER, 0,             NAME,  0, STD,  95,   0,  23, 250, 32, 3,  "Chiller Name:", RIGHT,   -8, 5, 0, LEFT, 4, 5, "Name of the chiller; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 12873, 12873, 0, 1, CHILLER, 0,             TYPE,  0, STD,  95,  25, 300, 180, 19, 3,          "Type:",  RIGHT,  -8, 5, 0, LEFT, 4, 5, "DOE-2 has models for many different types of chillers"

; AFR 7/21/09 - moved here from Compliance tab
    EDIT, 15498,     0, 0, 1, CHILLER, 0,   C-NUM-OF-UNITS, -1, STD, 490,   0,  23,  50,  0, 1, "Number of Chillers:",  RIGHT,  -5,  5, 1, LEFT, 4, 5, "The total number of chillers simulated as one unit"
   COMBO, 15500,     0, 0, 1, CHILLER, 0,           C-TYPE,  0, STD, 290,  25, 300, 180, 19, 1, "",                      LEFT, -90,  5, 0, LEFT, 4, 5, "The type of chiller"

    EDIT, 15501,     0, 0, 1, CHILLER, 0,            C-COP, -1, STD, 95,  50,  23,  60,  2, 1, "COP:",                   LEFT,  -35,  5, 1, LEFT, 4, 5, "The coefficient of performance of this chiller"
    EDIT, 15502,     0, 0, 1, CHILLER, 0,           C-IPLV, -1, STD, 95,  75,  23,  60,  2, 1, "IPLV:",                  LEFT,  -35,  5, 1, LEFT, 4, 5, "The integrated part load value of this chiller"


; SAC 10/28/01 - Added CASE statements by Chiller Type to accomodate differences in SubType compatibility for CHW-LOOP, HW-LOOP & CW-LOOP assignments -AND- for varying CONDENSER-TYPE symbol types
    CASE, CHILLER, 0, TYPE, -1, =, 1, 10    ; CHILLER:TYPE = HEAT-PUMP
       LABEL,  "Loop Assignments", STD, LEFT, 20, 100, 1, 0, 0, 210, 17515, 3
       COMBO, 17515, 19111, 0, 1, CHILLER, 10,         CHW-LOOP,  0, STD,  70, 120, 200, 140, 19, 3,                  "CHW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the primary Chiller Water Loop that this chiller serves"
       COMBO, 17516, 19112, 0, 1, CHILLER, 10,          CW-LOOP,  0, STD,  70, 145, 200, 140, 19, 3,                   "CW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "If Condenser Type=Water Cooled, CW Loop is required & must be attached to Heat Rejection"
       COMBO, 17517, 19117, 0, 1, CHILLER, 10,          HW-LOOP,  0, STD,  70, 170, 200, 140, 19, 3,                   "HW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the hot water loop that provides heat to the absorption chiller"
       COMBO, 17518, 19114, 0, 1, CHILLER, 10,       HTREC-LOOP,  0, STD,  70, 195, 200, 140, 19, 3,                "HtRec:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the Heat Recovery Loop that this chiller rejects heat to"
   
       LABEL, "Meter Assignments", STD, LEFT, 20, 225, 1, 0, 0, 210, 17519, 3
       COMBO, 17519, 12948, 0, 1, CHILLER, 10,       ELEC-METER,  0, STD, 135, 245, 120,  75, 19, 3,       "Electric Meter:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electric consumption of this chiller"
       COMBO, 17520, 12949, 0, 1, CHILLER, 10,       FUEL-METER,  0, STD, 135, 270, 120,  75, 19, 3,           "Fuel Meter:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Name of the Fuel Meter that tallies the fuel consumpton of this chiller"
   
;      COMBO, 17521, 13799, 0, 1, CHILLER, 10,        COST-DATA,  0, STD,  70, 295, 120, 140, 19, 3,                 "Cost:",  LEFT,  -50, 5, 0, LEFT, 4, 5, ""
   
       LABEL, "Equipment Capacity", STD, LEFT, 250, 50, 1, 0, 0, 435, 17522, 3
        EDIT, 17522, 13792, 0, 1, CHILLER, 10,         CAPACITY, -1, STD, 325,  70,  23,  70,  1, 3,             "Capacity:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Nominal (rated) chiller cooling capacity in MBTU/hr (e.g., 100 ton=1.2MBTU/hr)"
        EDIT, 17523, 13793, 0, 1, CHILLER, 10,   CAPACITY-RATIO, -1, STD, 350,  95,  23,  45,  2, 3,       "Capacity Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Capacity as fraction of max cooling load (used only if DOE-2 sizes the chiller)"
; SAC 10/28/01 - Added new HEAT/COOL-CAP keyword
        EDIT, 17645,     0, 0, 1, CHILLER, 10,    HEAT/COOL-CAP, -1, STD, 350, 120,  23,  45,  2, 3,        "Heat/Cool Cap:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Ratio of heating capacity to the cooling capacity at standard rating conditions"

       LABEL, "Equipment Efficiency", STD, LEFT, 480, 50, 1, 0, 0, 675, 17528, 3
        EDIT, 17528, 12879, 0, 1, CHILLER, 10, ELEC-INPUT-RATIO, -1, STD, 590,  70,  23,  60,  4, 3,     "Elec Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to nominal capacity (i.e., inverse of COP)"
        EDIT, 17529, 12956, 0, 1, CHILLER, 10, HEAT-INPUT-RATIO, -1, STD, 590,  95,  23,  60,  4, 3,     "Heat Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Ratio of fuel heat input (in Btus) to full load cooling capacity (in Btus), at rated conditions"
; SAC 10/28/01 - Added new HEAT-EIR keyword
        EDIT, 17648,     0, 0, 1, CHILLER, 10,         HEAT-EIR, -1, STD, 590, 120,  23,  60,  4, 3,          "Heating EIR:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to heating capacity at standard heating rating conditions"
    ENDCASE
   
    CASE, CHILLER, 0, TYPE, -1, =, 1, 11    ; CHILLER:TYPE = LOOP-TO-LOOP-HP
       LABEL,  "Loop Assignments", STD, LEFT, 20, 100, 1, 0, 0, 210, 17540, 3
       COMBO, 17540, 19111, 0, 1, CHILLER, 11,         CHW-LOOP,  0, STD,  70, 120, 200, 140, 19, 3,                  "CHW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the primary Chiller Water Loop that this chiller serves"
       COMBO, 17541, 19112, 0, 1, CHILLER, 11,          CW-LOOP,  0, STD,  70, 145, 200, 140, 19, 3,                   "CW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "If Condenser Type=Water Cooled, CW Loop is required & must be attached to Heat Rejection"
       COMBO, 17542, 19117, 0, 1, CHILLER, 11,          HW-LOOP,  0, STD,  70, 170, 200, 140, 19, 3,                   "HW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the hot water loop that provides heat to the absorption chiller"
       COMBO, 17543, 19114, 0, 1, CHILLER, 11,       HTREC-LOOP,  0, STD,  70, 195, 200, 140, 19, 3,                "HtRec:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the Heat Recovery Loop that this chiller rejects heat to"
   
       LABEL, "Meter Assignments", STD, LEFT, 20, 225, 1, 0, 0, 210, 17544, 3
       COMBO, 17544, 12948, 0, 1, CHILLER, 11,       ELEC-METER,  0, STD, 135, 245, 120,  75, 19, 3,       "Electric Meter:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electric consumption of this chiller"
       COMBO, 17545, 12949, 0, 1, CHILLER, 11,       FUEL-METER,  0, STD, 135, 270, 120,  75, 19, 3,           "Fuel Meter:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Name of the Fuel Meter that tallies the fuel consumpton of this chiller"
   
;      COMBO, 17546, 13799, 0, 1, CHILLER, 11,        COST-DATA,  0, STD,  70, 295, 120, 140, 19, 3,                 "Cost:",  LEFT,  -50, 5, 0, LEFT, 4, 5, ""
   
       LABEL, "Equipment Capacity", STD, LEFT, 250, 50, 1, 0, 0, 435, 17547, 3
        EDIT, 17547, 13792, 0, 1, CHILLER, 11,         CAPACITY, -1, STD, 325,  70,  23,  70,  1, 3,             "Capacity:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Nominal (rated) chiller cooling capacity in MBTU/hr (e.g., 100 ton=1.2MBTU/hr)"
        EDIT, 17548, 13793, 0, 1, CHILLER, 11,   CAPACITY-RATIO, -1, STD, 350,  95,  23,  45,  2, 3,       "Capacity Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Capacity as fraction of max cooling load (used only if DOE-2 sizes the chiller)"
; SAC 10/28/01 - Added new HEAT/COOL-CAP keyword
        EDIT, 17646,     0, 0, 1, CHILLER, 11,    HEAT/COOL-CAP, -1, STD, 350, 120,  23,  45,  2, 3,        "Heat/Cool Cap:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Ratio of heating capacity to the cooling capacity at standard rating conditions"
   
       LABEL, "Equipment Efficiency", STD, LEFT, 480, 50, 1, 0, 0, 675, 17553, 3
        EDIT, 17553, 12879, 0, 1, CHILLER, 11, ELEC-INPUT-RATIO, -1, STD, 590,  70,  23,  60,  4, 3,     "Elec Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to nominal capacity (i.e., inverse of COP)"
        EDIT, 17554, 12956, 0, 1, CHILLER, 11, HEAT-INPUT-RATIO, -1, STD, 590,  95,  23,  60,  4, 3,     "Heat Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Ratio of fuel heat input (in Btus) to full load cooling capacity (in Btus), at rated conditions"
; SAC 10/28/01 - Added new HEAT-EIR keyword
        EDIT, 17648,     0, 0, 1, CHILLER, 11,         HEAT-EIR, -1, STD, 590, 120,  23,  60,  4, 3,          "Heating EIR:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to heating capacity at standard heating rating conditions"
    ENDCASE

    CASE, CHILLER, 0, TYPE, -1, =, 1, 13    ; CHILLER:TYPE = WATER-ECONOMIZER

       LABEL,  "Loop Assignments", STD, LEFT, 20, 100, 1, 0, 0, 210, 17840, 3
       COMBO, 17840, 19111, 0, 1, CHILLER, 13,         CHW-LOOP,  0, STD,  70, 120, 200, 140, 19, 3,                  "CHW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the primary Chiller Water Loop that this chiller serves"
       COMBO, 17841, 19112, 0, 1, CHILLER, 13,          CW-LOOP,  0, STD,  70, 145, 200, 140, 19, 3,                   "CW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "If Condenser Type=Water Cooled, CW Loop is required & must be attached to Heat Rejection"
       COMBO, 17842, 19117, 0, 1, CHILLER, 13,          HW-LOOP,  0, STD,  70, 170, 200, 140, 19, 3,                   "HW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the hot water loop that provides heat to the absorption chiller"
       COMBO, 17843, 19114, 0, 1, CHILLER, 13,       HTREC-LOOP,  0, STD,  70, 195, 200, 140, 19, 3,                "HtRec:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the Heat Recovery Loop that this chiller rejects heat to"
   
       LABEL, "Meter Assignments", STD, LEFT, 20, 225, 1, 0, 0, 210, 17845, 3
       COMBO, 17845, 12948, 0, 1, CHILLER, 13,       ELEC-METER,  0, STD, 135, 245, 120,  75, 19, 3,       "Electric Meter:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electric consumption of this chiller"
       COMBO, 17846, 12949, 0, 1, CHILLER, 13,       FUEL-METER,  0, STD, 135, 270, 120,  75, 19, 3,           "Fuel Meter:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Name of the Fuel Meter that tallies the fuel consumpton of this chiller"
   
       LABEL, "Equipment Efficiency", STD, LEFT, 250, 50, 1, 0, 0, 445, 17848, 3
; SAC 11/19/10 - removed from design sizing D2 detailed UI
;        EDIT, 17848,     0, 0, 1, CHILLER, 13,  WATER-ECONO-EFF, -1, STD, 360,  70,  23,  60,  4, 3,     "HX Effectiveness:",  LEFT, -110, 5, 1, LEFT, 4, 5, "heat exchanger effectiveness (constant for all CHW & CW flows)"

       LABEL, "Equipment Capacity", STD, LEFT, 490, 25, 1, 0, 0, 675, 17850, 3
        EDIT, 17850, 13792, 0, 1, CHILLER, 13,         CAPACITY, -1, STD, 565,  45,  23,  70,  1, 3,             "Capacity:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Nominal (rated) chiller cooling capacity in MBTU/hr (e.g., 100 ton=1.2MBTU/hr)"
        EDIT, 17851, 13793, 0, 1, CHILLER, 13,   CAPACITY-RATIO, -1, STD, 590,  70,  23,  45,  2, 3,       "Capacity Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Capacity as fraction of max cooling load (used only if DOE-2 sizes the chiller)"

    ENDCASE





;    3> DESIGN-CHW-T              F           Numnric Err,Cau    1           20.00           50.00   3  -77777.00 *No Default*    
;    4> DESIGN-HW-T               F           Numnric Err,Cau    1           80.10           40.00   4  -88888.00 *  Unused  *    
;    5> DESIGN-COND-T             F           Numnric Err,Cau    1           30.00           85.00   5  -77777.00 *No Default*    
;    6> DESIGN-COND-T-HT          F           Numnric Err,Cau    1           30.00           85.00   6  -88888.00 *  Unused  *    
;    7> DESIGN-PLR                FRAC.OR MUL Numeric Err,Err    1            0.70            1.00   7  -88888.00 *  Unused  *    
;    8> RATED-CHW-T               F           Numnric Err,Cau    1           20.00           50.00   8      44.00                 
;    9> RATED-HW-T                F           Numnric Err,Cau    1           80.00            0.01   9  -88888.00 *  Unused  *    
;   10> RATED-COND-T              F           Numnric Err,Cau    1           30.00           85.00  10  -77777.00 *No Default*    
;   11> RATED-COND-T-HT           F           Numnric Err,Cau    1           32.00           70.00  11  -88888.00 *  Unused  *    
;   12> RATED-CW-FLOW             GALLONS/MIN Numeric Err,Err    1            1.00            6.00  12  -77777.00 *No Default*    
;   13> RATED-HT/CL-FLOW          FRAC.OR MUL Numnric Err,Cau    1            0.40            2.00  13  -88888.00 *  Unused  *    
;   14> SPECIFIED-AT                        Symbolic Defined    1 3105 (CODE-WORD       )  TABLE =0   14        990 (RATED-CONDITIONS)
;                                SYMBOL TABLE ENTRY   RATED-CONDITIONS                 TYPE = 3105 DEF/REF  -1/ -1      VALUE =    1
;                                SYMBOL TABLE ENTRY   DESIGN-CONDITIONS                TYPE = 3105 DEF/REF  -1/ -1      VALUE =    2



    CASE, ELSE
       LABEL,  "Loop Assignments", STD, LEFT, 20, 100, 1, 0, 0, 210, 19125, 3
       COMBO, 19125, 19111, 0, 1, CHILLER,  0,         CHW-LOOP,  0, STD,  70, 120, 200, 140, 19, 3,                  "CHW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the primary Chiller Water Loop that this chiller serves"
       COMBO, 19126, 19112, 0, 1, CHILLER,  0,          CW-LOOP,  0, STD,  70, 145, 200, 140, 19, 3,                   "CW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "If Condenser Type=Water Cooled, CW Loop is required & must be attached to Heat Rejection"
       COMBO, 19127, 19117, 0, 1, CHILLER,  0,          HW-LOOP,  0, STD,  70, 170, 200, 140, 19, 3,                   "HW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the hot water loop that provides heat to the absorption chiller"
       COMBO, 19128, 19114, 0, 1, CHILLER,  0,       HTREC-LOOP,  0, STD,  70, 195, 200, 140, 19, 3,                "HtRec:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the Heat Recovery Loop that this chiller rejects heat to"
   
       LABEL, "Meter Assignments", STD, LEFT, 20, 225, 1, 0, 0, 210, 12948, 3
       COMBO, 12948, 12948, 0, 1, CHILLER,  0,       ELEC-METER,  0, STD, 135, 245, 120,  75, 19, 3,       "Electric Meter:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electric consumption of this chiller"
       COMBO, 12949, 12949, 0, 1, CHILLER,  0,       FUEL-METER,  0, STD, 135, 270, 120,  75, 19, 3,           "Fuel Meter:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Name of the Fuel Meter that tallies the fuel consumpton of this chiller"
   
; SAC 5/13/10 - comment out access to PERFORMANCE-DATA components until implementation completed
;; JJH added performance data reference
;      LABEL,    "Performance Data", STD, LEFT, 20, 315, 1, 0, 0, 250, 0, 3
;      COMBO, 18971, 13108, 0, 1, CHILLER, 0, PERFORM-DATA-WC , 0, STD, 100, 330,  80, 150, 19, 3,     "Wtr Cooled:", LEFT, -80, 5, 0, LEFT, 4, 5, ""
;      COMBO, 18972, 13108, 0, 1, CHILLER, 0, PERFORM-DATA-AC , 0, STD, 100, 355,  80, 150, 19, 3,     "Air Cooled:", LEFT, -80, 5, 0, LEFT, 4, 5, ""

;      COMBO, 12070, 13799, 0, 1, CHILLER,  0,        COST-DATA,  0, STD,  70, 295, 120, 140, 19, 3,                 "Cost:",  LEFT,  -50, 5, 0, LEFT, 4, 5, ""
   
   
;        LABEL, "Equipment Capacity", STD, LEFT, 250, 50, 1, 0, 0, 435, 12950, 3
;         EDIT, 12950, 13792, 0, 1, CHILLER,  0,         CAPACITY, -1, STD, 325,  70,  23,  70,  1, 3,             "Capacity:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Nominal (rated) chiller cooling capacity in MBTU/hr (e.g., 100 ton=1.2MBTU/hr)"
;         EDIT, 12951, 13793, 0, 1, CHILLER,  0,   CAPACITY-RATIO, -1, STD, 350,  95,  23,  45,  2, 3,       "Capacity Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Capacity as fraction of max cooling load (used only if DOE-2 sizes the chiller)"
;         EDIT, 12953, 12953, 0, 1, CHILLER,  0,        MIN-RATIO, -1, STD, 350, 120,  23,  45,  2, 3,            "Min Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Minimum chiller operating ratio (a fraction of the Capacity); below this, it cycles on & off"
;         EDIT, 12952, 12952, 0, 1, CHILLER,  0,        HGB-RATIO, -1, STD, 350, 145,  23,  45,  2, 3,            "HGB Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Maximum allowable part-load ratio of the chiller, above which hot gas bypass occurs"
;         EDIT, 12970, 12970, 0, 1, CHILLER,  0,  HGB-RATIO-HTREC, -1, STD, 350, 170,  23,  45,  2, 3,         "HGB Ratio HR:",  LEFT, -100, 5, 1, LEFT, 4, 5, "The hot gas bypass ratio when the chiller is in the heat recovery mode"
; ; SAC 10/28/01 - Added new HEAT/COOL-CAP keyword
;         EDIT, 17647,     0, 0, 1, CHILLER,  0,    HEAT/COOL-CAP, -1, STD, 350, 195,  23,  45,  2, 3,        "Heat/Cool Cap:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Ratio of heating capacity to the cooling capacity at standard rating conditions"


       LABEL, "Equipment Efficiency", STD, LEFT, 250, 50, 1, 0, 0, 445, 12955, 3
        EDIT, 12955, 12879, 0, 1, CHILLER,  0, ELEC-INPUT-RATIO, -1, STD, 360,  70,  23,  60,  4, 3,     "Elec Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to nominal capacity (i.e., inverse of COP)"
        EDIT, 12956, 12956, 0, 1, CHILLER,  0, HEAT-INPUT-RATIO, -1, STD, 360,  95,  23,  60,  4, 3,     "Heat Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Ratio of fuel heat input (in Btus) to full load cooling capacity (in Btus), at rated conditions"
; SAC 10/28/01 - Added new HEAT-EIR keyword
        EDIT, 17648,     0, 0, 1, CHILLER,  0,         HEAT-EIR, -1, STD, 360, 120,  23,  60,  4, 3,          "Heating EIR:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to heating capacity at standard heating rating conditions"
; JJH 7/06/06 - Add VARIABLE-SPEED related keywords
       LABEL, "Compressor Configuration", STD, LEFT, 250, 152, 1, 0, 0, 445, 18235, 3
       COMBO, 18234,     0, 0, 1, CHILLER,  0,  COMPRESSORS/CKT, -1, STD, 360, 170, 200,  85, 19, 3,      "Compressors/Ckt:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Specifies the number of compressors used per refrigerant curcuit"

;       LABEL, "Design vs. Rated Conditions", STD, LEFT, 250, 225, 1, 0, 0, 675, 0, 3   ; SAC 11/24/10 - removed
;       COMBO, 17695,     0, 0, 1, CHILLER,  0,     SPECIFIED-AT,  0, STD, 390, 245, 120, 140, 19, 3, "Chiller Specified At:",  LEFT, -125, 5, 0, LEFT, 4, 5, "The conditions at which the user is specifying the chiller"   ; SAC 11/24/10 - removed

       LABEL, "Design Conditions", STD, LEFT, 265, 275, 1, 0, 0, 455, 17696, 3
        EDIT, 17696,     0, 0, 1, CHILLER,  0,    DESIGN-CHW-T , -1, STD, 375, 295,  23,  55,  1, 3,     "Chilled-Wtr Temp:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Leaving chilled-water temperature at the DESIGN conditions"
        EDIT, 17697,     0, 0, 1, CHILLER,  0,    DESIGN-COND-T, -1, STD, 375, 320,  23,  55,  1, 3,     "Condenser Temp:",    LEFT, -110, 5, 1, LEFT, 4, 5, "Condenser temperature at the DESIGN conditions"
;        EDIT, 17698,     0, 0, 1, CHILLER,  0,    DESIGN-PLR   , -1, STD, 375, 345,  23,  55,  3, 3,     "Design/Max Cap:",    LEFT, -110, 5, 1, LEFT, 4, 5, "The ratio of the DESIGN capacity to the maximum capacity"   ; SAC 11/24/10 - removed
        EDIT, 19281,     0, 0, 1, CHILLER,  0,    DESIGN-WELL-T, -1, STD, 375, 345,  23,  55,  1, 3,     "Well Temp:",         LEFT, -110, 5, 1, LEFT, 4, 5, "Design water temperature provided by the well when cooling-dominated.  Default is the temperature provided by the LAKE/WELL."
        EDIT, 19282,     0, 0, 1, CHILLER,  0, DESIGN-WELL-T-HT, -1, STD, 375, 370,  23,  55,  1, 3,     "Well Temp Heatg:",   LEFT, -110, 5, 1, LEFT, 4, 5, "Design water temperature provided by the well when heating-dominated.  Default is the temperature provided by the LAKE/WELL."

;       LABEL, "Rated Conditions", STD, LEFT, 485, 275, 1, 0, 0, 675, 17699, 3
;        EDIT, 17699,     0, 0, 1, CHILLER,  0,    RATED-CHW-T  , -1, STD, 595, 295,  23,  55,  1, 3,     "Chilled-Wtr Temp:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Leaving chilled-water temperature at the RATED conditions"
;        EDIT, 17700,     0, 0, 1, CHILLER,  0,    RATED-COND-T , -1, STD, 595, 320,  23,  55,  1, 3,     "Condenser Temp:",    LEFT, -110, 5, 1, LEFT, 4, 5, "Condenser temperature at the RATED conditions"
;        EDIT, 17701,     0, 0, 1, CHILLER,  0,    RATED-CW-FLOW, -1, STD, 595, 345,  23,  55,  2, 3,     "Condenser Flow:",    LEFT, -110, 5, 1, LEFT, 4, 5, "Condenser flow at the RATED conditions (for water-cooled condensers)"

       LABEL, "Equipment Capacity", STD, LEFT, 490, 25, 1, 0, 0, 675, 12950, 3
        EDIT, 12950, 13792, 0, 1, CHILLER,  0,         CAPACITY, -1, STD, 565,  45,  23,  70,  1, 3,             "Capacity:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Nominal (rated) chiller cooling capacity in MBTU/hr (e.g., 100 ton=1.2MBTU/hr)"
        EDIT, 12951, 13793, 0, 1, CHILLER,  0,   CAPACITY-RATIO, -1, STD, 590,  70,  23,  45,  2, 3,       "Capacity Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Capacity as fraction of max cooling load (used only if DOE-2 sizes the chiller)"
; SAC 10/28/01 - Added new HEAT/COOL-CAP keyword
        EDIT, 17647,     0, 0, 1, CHILLER,  0,    HEAT/COOL-CAP, -1, STD, 590,  95,  23,  45,  2, 3,        "Heat/Cool Cap:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Ratio of heating capacity to the cooling capacity at standard rating conditions"

; SAC 7/6/06 - revision to JJH mods to ensure VARIABLE-SPEED combo displays correct set of symbol selections
       CASE, CHILLER, 0, TYPE, -1, =, 1, 1    ; CHILLER:TYPE = OPEN-CENT
          COMBO, 18233,     0, 0, 1, CHILLER,  1,   VARIABLE-SPEED, -1, STD, 360, 195, 160, 160, 19, 3,       "VSD Drive Used:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Specifies that a variable speed drive is installed, and the type of compressor being used (Centrifugal chillers only)"
       ENDCASE
       CASE, CHILLER, 0, TYPE, -1, =, 1, 3    ; CHILLER:TYPE = ELEC-HERM-CENT
          COMBO, 18236,     0, 0, 1, CHILLER,  3,   VARIABLE-SPEED, -1, STD, 360, 195, 160, 160, 19, 3,       "VSD Drive Used:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Specifies that a variable speed drive is installed, and the type of compressor being used (Centrifugal chillers only)"
       ENDCASE
       CASE, ELSE
          COMBO, 18237,     0, 0, 1, CHILLER,  0,   VARIABLE-SPEED, -1, STD, 360, 195, 160, 160, 19, 3,       "VSD Drive Used:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Specifies that a variable speed drive is installed, and the type of compressor being used (Centrifugal chillers only)"
       ENDCASE

    ENDCASE


;   --------------------------------------------------------------
;
; SAC TO DO - Need to add access to these keywords via the CHILLER spreadsheet(s)
;
;   --------------------------------------------------------------
;   NEW CHILLER KEYWORDS:
;   --------------------------------------------------------------
;           EDIT, 17647,     0, 0, 1, CHILLER,  0,    HEAT/COOL-CAP, -1, STD, 350, 195,  23,  45,  2, 3,        "Heat/Cool Cap:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Ratio of heating capacity to the cooling capacity at standard rating conditions"
;           EDIT, 17648,     0, 0, 1, CHILLER,  0,         HEAT-EIR, -1, STD, 590, 120,  23,  60,  4, 3,          "Heating EIR:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to heating capacity at standard heating rating conditions"
;   
;   
;      LABEL, "Electric Heating Capacity", STD, CENTER, 415, 275, 1, 0, 0, 0, 17654, 3
;      COMBO, 17654,     0, 0, 1, CHILLER, 0,      HEAT-CAP-FT,  0, STD, 335, 295, 200, 165, 19, 3,  "",  LEFT, -315,  5, 0, LEFT, 4, 5, "Electric Heating Capacity as a function of leaving hot water and entering air temperatures (no frost on heat exchanger)"
;      COMBO, 17655,     0, 0, 1, CHILLER, 0, HEAT-CAP-FT-FRST,  0, STD, 335, 325, 200, 165, 19, 3,  "",  LEFT, -315,  5, 0, LEFT, 4, 5, "Electric Heating Capacity as a function of leaving hot water and entering air temperatures (when frost forms on heat exchanger)"
;   
;      LABEL, "Heating Elec Input Ratio", STD, CENTER, 230, 275, 1, 0, 0, 0, 17651, 3
;      COMBO, 17651,     0, 0, 1, CHILLER, 0,      HEAT-EIR-FT,  0, STD, 150, 295, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Heating Electric Input Ratio as a function of leaving hot water and entering air temperatures (no frost on heat exchanger)"
;      LABEL,  "f(t leaving HW,",       STD, LEFT, 20, 292, 1, 0, 0, 0, 0, 3
;      LABEL,  "t entering air) nf:",   STD, LEFT, 30, 306, 1, 0, 0, 0, 0, 3
;      COMBO, 17652,     0, 0, 1, CHILLER, 0, HEAT-EIR-FT-FRST,  0, STD, 150, 325, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Heating Electric Input Ratio as a function of leaving hot water and entering air temperatures (when frost forms on heat exchanger)"
;      LABEL,  "f(t leaving HW,",       STD, LEFT, 20, 322, 1, 0, 0, 0, 0, 3
;      LABEL,  "t entering air) frst:", STD, LEFT, 30, 336, 1, 0, 0, 0, 0, 3
;      COMBO, 17653,     0, 0, 1, CHILLER, 0,    HEAT-EIR-FPLR,  0, STD, 150, 355, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Heating Electric Input Ratio as a function of the heating part load ratio"
;      LABEL,  "f(part load ratio):",   STD, LEFT, 20, 360, 1, 0, 0, 0, 0, 3
;   
;   
;      LABEL, "Heat Exchangers (counterflow)", STD, LEFT, 180, 275, 1, 0, 0, 580, 0, 3
;      LABEL, "Evaporator", STD, CENTER, 450, 295, 1, 0, 0, 0, 17656, 3
;       EDIT, 17656,     0, 0, 1, CHILLER, 0,       EVAP-HX-TD, -1, STD, 420, 315,  23,  60,  2, 3,  "Design Temperature Differential:", LEFT, -220, 5, 1, LEFT, 4, 5, ""
;       EDIT, 17657,     0, 0, 1, CHILLER, 0,  EVAP-HX-SETPT-T, -1, STD, 420, 340,  23,  60,  2, 3,             "Setpoint Temperature:", LEFT, -220, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Condenser",  STD, CENTER, 530, 295, 1, 0, 0, 0, 17658, 3
;       EDIT, 17658,     0, 0, 1, CHILLER, 0,       COND-HX-TD, -1, STD, 500, 315,  23,  60,  2, 3,                                  "", LEFT,   -1, 5, 1, LEFT, 4, 5, ""
;       EDIT, 17659,     0, 0, 1, CHILLER, 0,  COND-HX-SETPT-T, -1, STD, 500, 340,  23,  60,  2, 3,                                  "", LEFT,   -1, 5, 1, LEFT, 4, 5, ""
;   
;   
;           EDIT, 17641,     0, 0, 1, CHILLER,  0,     COND-CAPACITY, -1, STD, 590, 295,  23,  60,  1, 3,             "Capacity:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
;           EDIT, 17642,     0, 0, 1, CHILLER,  0,      COND-FAN-EIR, -1, STD, 590, 320,  23,  60,  4, 3,              "Fan EIR:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
;           EDIT, 17643,     0, 0, 1, CHILLER,  0,     COND-PUMP-EIR, -1, STD, 590, 345,  23,  60,  4, 3,             "Pump EIR:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
;   
;   --------------------------------------------------------------


; --------------------------------------------------------------
; SAC 10/28/01 - NOT YET IMPLEMENTED
; --------------------------------------------------------------
;   71> COND-SETPT-CTRL                     Symbolic Defined    1  272 (CODE-WORD       )  TABLE =0   71         -7 (*No Default*    )
;                                SYMBOL TABLE ENTRY   FIXED                            TYPE =  272 DEF/REF  -1/ -1      VALUE =    0
;                                SYMBOL TABLE ENTRY   VARIABLE                         TYPE =  272 DEF/REF  -1/ -1      VALUE =    1
;                                SYMBOL TABLE ENTRY   AMBIENT                          TYPE =  272 DEF/REF  -1/ -1      VALUE =    2
;   72> COND-FAN-CTRL                       Symbolic Defined    1 2130 (CODE-WORD       )  TABLE =0   72         -7 (*No Default*    )
;                                SYMBOL TABLE ENTRY   DAMPER-MODULATION                TYPE = 2130 DEF/REF  -1/ -1      VALUE =    1
;                                SYMBOL TABLE ENTRY   PRESSURE-SWITCHES                TYPE = 2130 DEF/REF  -1/ -1      VALUE =    2
;                                SYMBOL TABLE ENTRY   TWO-SPEED-FANS                   TYPE = 2130 DEF/REF  -1/ -1      VALUE =    3
;                                SYMBOL TABLE ENTRY   VFD-ON-FANS                      TYPE = 2130 DEF/REF  -1/ -1      VALUE =    4
;   73> COND-SETPT-T              F           Numnric Err,Cau    1           60.00          130.00  73  -77777.00 *No Default*    
;   74> COND-SETPT-DT             F (DELTA)   Numnric Err,Cau    1            0.00           30.00  74  -77777.00 *No Default*    
;   75> MIN-COND-T                F           Numnric Err,Cau    1           60.00          130.00  75  -77777.00 *No Default*    
;   77> SCT-AMB-DT                F (DELTA)   Numnric Err,Cau    1            5.00           40.00  77  -77777.00 *No Default*    
;   80> COND-CAP-FT                         Symbolic Undef      1   60 (CURVE-FIT       )  TABLE =4   80         -7 (*No Default*    )
;   81> AMB-FRAC-FT                         Symbolic Undef      1   60 (CURVE-FIT       )  TABLE =4   81         -7 (*No Default*    )
;   82> COND-PWR-FPLR                       Symbolic Undef      1   60 (CURVE-FIT       )  TABLE =4   82         -7 (*No Default*    )
; --------------------------------------------------------------


; SAC 11/30/10 - ported over rated perf tab from prev. des sizing version - 1/16/06 - Design sizing mods - entirely new tab
    ;******************************************
    ; Chiller - Rated Performance Page
    ;******************************************
    TABPAGE, 3366, 3366, 1, 3, NOTIMP, " Rated Performance "

    LABEL, "Capacity (choose ONE):", STD, LEFT,  15,  10, 1, 0, 0, 230, 0, 3
     EDIT, 18072, 13792, 0, 1, CHILLER,  0,         CAPACITY, -1, STD,  95,  30,  23,  95,  3, 3,             "Capacity:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "The rated capacity in million of Btu/hr (English) or kW (metric)"
     EDIT, 18073,     0, 0, 1, CHILLER,  0,             TONS, -1, STD,  95,  55,  23,  95,  2, 3,                 "Tons:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "The rated capacity in tons (English only)"
     EDIT, 18074, 13793, 0, 1, CHILLER,  0,   CAPACITY-RATIO, -1, STD, 130,  80,  23,  60,  3, 3,       "Capacity Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "The fraction of design-day load"
     EDIT, 18075,     0, 0, 1, CHILLER,  0,        RATED-PLR, -1, STD, 130, 105,  23,  60,  3, 3,    "Rated Part-Ld Rat:",  LEFT, -110, 5, 1, LEFT, 4, 5, "The ratio of the rated capacity to the maximum capacity, at rated conditions"

    LABEL, "Rated Conditions", STD, LEFT, 275,  10, 1, 0, 0, 680, 0, 3
    LABEL, "Chilled Wtr", STD, CENTER, 420,  23, 1, 0, 0, 0, 0, 3
    LABEL, "Condenser",   STD, CENTER, 490,  23, 1, 0, 0, 0, 0, 3
    LABEL, "Hot Water",   STD, CENTER, 560,  23, 1, 0, 0, 0, 0, 3
     EDIT, 17699,     0, 0, 1, CHILLER,  0,  RATED-CHW-T,     -1, STD, 390,  40,  23,  60,  2, 3,          "Temperature:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Leaving chilled-water temperature at the RATED conditions"
     EDIT, 17700,     0, 0, 1, CHILLER,  0,  RATED-CHW-FLOW,  -1, STD, 390,  65,  23,  60,  2, 3,           "Fluid Flow:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Chilled-water flow at the RATED conditions (affects head only)"
     EDIT, 17701,     0, 0, 1, CHILLER,  0,  RATED-CHW-DT,    -1, STD, 390,  90,  23,  60,  2, 3,              "Delta-T:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Chilled-water temperature drop at the RATED conditions; alternative to 'Chilled-Wtr Flow'"
     EDIT, 18076,     0, 0, 1, CHILLER,  0,  RATED-COND-T,    -1, STD, 460,  40,  23,  60,  2, 3,                      "",  LEFT,    0, 5, 0, LEFT, 4, 5, "Entering condenser temperature, or saturated temperature, at the RATED conditions"
     EDIT, 18077,     0, 0, 1, CHILLER,  0,  RATED-CW-FLOW,   -1, STD, 460,  65,  23,  60,  2, 3,                      "",  LEFT,    0, 5, 1, LEFT, 4, 5, "Condenser flow at the RATED conditions, water-cooled condenser"
     EDIT, 18078,     0, 0, 1, CHILLER,  0,  RATED-CW-DT,     -1, STD, 460,  90,  23,  60,  2, 3,                      "",  LEFT,    0, 5, 0, LEFT, 4, 5, "Condenser temperature change at the RATED conditions; alternative to 'Condenser Flow'"
     EDIT, 18079,     0, 0, 1, CHILLER,  0,  RATED-HW-T,      -1, STD, 530,  40,  23,  60,  2, 3,                      "",  LEFT,    0, 5, 1, LEFT, 4, 5, "Leaving hot-water temperature at the RATED conditions"
     EDIT, 18080,     0, 0, 1, CHILLER,  0,  RATED-HW-DT,     -1, STD, 530,  90,  23,  60,  2, 3,                      "",  LEFT,    0, 5, 1, LEFT, 4, 5, "Hot-water temperature rise at the RATED conditions"

    LABEL, "Loading Characteristics", STD, LEFT, 275, 126, 1, 0, 0, 680, 0, 3
;    COMBO, 18081,     0, 0, 1, CHILLER,  0,  VARIABLE-SPEED,  -1, STD, 415, 144, 120,  75, 19, 3,       "Variable Speed?",  LEFT, -130, 5, 0, LEFT, 4, 5, "Whether or not the chiller has a variable speed compressor"
    COMBO, 18082,     0, 0, 1, CHILLER,  0,  COMPRESSORS/CKT, -1, STD, 415, 169, 120,  75, 19, 3,  "Compressors per Ckt:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Determines which default part-load performance curve will be selected (assumes two circuits)"
     EDIT, 13644, 13644, 0, 1, CHILLER,  0,  START-UP-TIME,   -1, STD, 415, 194,  23,  50,  3, 3,        "Start-Up Time:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Equivalent full-load time required to start up the chiller (in hours or fraction of hours)"
     EDIT, 17890, 13644, 0, 1, CHILLER,  0,    STANDBY-TIME,  -1, STD, 415, 219,  23,  50,  3, 3,         "Standby Time:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Equivalent full-load time required to keep the chiller on-line with no load (in hours or fraction of hours)"
     EDIT, 13649, 13649, 0, 1, CHILLER,  0,  SHUT-DOWN-TIME,  -1, STD, 415, 244,  23,  50,  3, 3,       "Shut-Down Time:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Equivalent full-load time required to shut down the chiller (in hours or fraction of hours)"

     EDIT, 17524, 12953, 0, 1, CHILLER,  0,  MIN-RATIO,       -1, STD, 610, 144,  23,  45,  2, 3,            "Min Ratio:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "Minimum chiller operating ratio (a fraction of the Capacity); below this, it cycles on & off"
     EDIT, 17526, 12952, 0, 1, CHILLER,  0,  HGB-RATIO,       -1, STD, 610, 169,  23,  45,  2, 3,            "HGB Ratio:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "Maximum allowable part-load ratio of the chiller, above which hot gas bypass occurs"
     EDIT, 17527, 12970, 0, 1, CHILLER,  0,  HGB-RATIO-HTREC, -1, STD, 610, 194,  23,  45,  2, 3,         "HGB Ratio HR:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "The hot gas bypass ratio when the chiller is in the heat recovery mode"

    LABEL, "Heat Pump Chiller in Heating Mode", STD, LEFT, 275, 279, 1, 0, 0, 720, 18083, 3
    LABEL, "Capacity and Rated Conditions:",    STD, LEFT, 290, 294, 1, 0, 0,   0, 18083, 3
     EDIT, 18083,     0, 0, 1, CHILLER,  0, HEAT/COOL-CAP,    -1, STD, 395, 312,  23,  60,  3, 3,        "Heat/Cool Cap:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Ratio of heating capacity at heating rated condtions to cooling capacity at cooling rated conditions"
     EDIT, 18084,     0, 0, 1, CHILLER,  0, RATED-COND-T-HT,  -1, STD, 395, 337,  23,  60,  1, 3,            "Cond Temp:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The entering condenser temperature at the RATED heating conditions"
     EDIT, 18085,     0, 0, 1, CHILLER,  0, RATED-HT/CL-FLOW, -1, STD, 395, 362,  23,  60,  2, 3,        "Cond Flow Rat:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The ratio of the condenser flow at the RATED heating conditions to the condenser flow at RATED cooling conditions"
     EDIT, 18086,     0, 0, 1, CHILLER,  0, RATED-CW-DT-HT,   -1, STD, 395, 387,  23,  60,  2, 3,         "Condenser dT:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The condenser temperature drop at the RATED heating conditions; alternative to 'Condenser Flow'"
    LABEL, "Electric Power (choose ONE):",      STD, LEFT, 525, 294, 1, 0, 0,   0, 18083, 3
     EDIT, 18087,     0, 0, 1, CHILLER,  0, HEAT-EIR,         -1, STD, 630, 312,  23,  60,  3, 3,       "Elec Input Rat:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to rated capacity (inverse of COP), heating mode"
     EDIT, 18088,     0, 0, 1, CHILLER,  0, HEAT-POWER,       -1, STD, 630, 337,  23,  60,  3, 3,           "Heat Power:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "Electric power, heating mode; valid only if capacity specified"
     EDIT, 18089,     0, 0, 1, CHILLER,  0, HEAT-EER,         -1, STD, 630, 362,  23,  60,  1, 3,       "Energy Eff Rat:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "Ratio of rated capacity in Btuh to power in kW (English only), heating mode"
     EDIT, 18090,     0, 0, 1, CHILLER,  0, HEAT-COP,         -1, STD, 630, 387,  23,  60,  4, 3,        "Coef of Perf.:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "Dimensionless ratio of rated capacity to power (inverse of ELEC-INPUT-RATIO), heating mode"

    LABEL, "Electric Power (choose ONE):", STD, LEFT,  15, 150, 1, 0, 0, 230, 0, 3
     EDIT, 18091, 12879, 0, 1, CHILLER,  0, ELEC-INPUT-RATIO, -1, STD, 130, 170,  23,  60,  4, 3,     "Elec Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to rated capacity (inverse of COP)"
     EDIT, 18092,     0, 0, 1, CHILLER,  0,            POWER, -1, STD, 130, 195,  23,  60,  3, 3,                "Power:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Determines which default part-load performance curve will be selected (assumes two circuits)"
     EDIT, 18093,     0, 0, 1, CHILLER,  0,           KW/TON, -1, STD, 130, 220,  23,  60,  3, 3,           "kW per Ton:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Ratio of power in kW to capacity in tons (English only)"
     EDIT, 18094,     0, 0, 1, CHILLER,  0, ENERGY-EFF-RATIO, -1, STD, 130, 245,  23,  60,  1, 3,     "Energy Eff Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Ratio of rated capacity in Btuh to power in kW (English only)"

    CASE, CHILLER, 0, TYPE, -1, =, 1, 6    ; CHILLER:TYPE = ABSOR-1   
       LABEL, "Heat/Fuel Consmp. (choose ONE):", STD, LEFT,  15, 290, 1, 0, 0, 230, 18095, 3
        EDIT, 18095, 12956, 0, 1, CHILLER,  0, HEAT-INPUT-RATIO, -1, STD, 130, 310,  23,  60,  4, 3,     "Heat Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of heat input to rated capacity(inverse of COP)"
; SAC 11/30/10 - added for DOE-2.3
        EDIT, 19275,     0, 0, 1, CHILLER,  0,       HEAT-INPUT, -1, STD, 130, 335,  23,  60,  4, 3,           "Heat Input:",  LEFT, -110, 5, 1, LEFT, 4, 5, "An alternative to HEAT-INPUT-RATIO, is the heat/fuel consumption of the chiller at the RATED conditions"
        EDIT, 18096,     0, 0, 1, CHILLER,  0,   COEF-OF-PERFOR, -1, STD, 130, 360,  23,  60,  4, 3,     "Coef of Perform.:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of rated capacity to heat consumption (inverse of HEAT-INPUT-RATIO)"
       COMBO, 18081,     0, 0, 1, CHILLER,  0,  VARIABLE-SPEED,  -1, STD, 415, 144, 120,  75, 19, 3,       "Variable Speed?",  LEFT, -130, 5, 0, LEFT, 4, 5, "Whether or not the chiller has a variable speed compressor"
    ENDCASE

    CASE, CHILLER, 0, TYPE, -1, =, 1, 7    ; CHILLER:TYPE = ABSOR-2   
       LABEL, "Heat/Fuel Consmp. (choose ONE):", STD, LEFT,  15, 290, 1, 0, 0, 230, 18097, 3
        EDIT, 18097, 12956, 0, 1, CHILLER,  0, HEAT-INPUT-RATIO, -1, STD, 130, 310,  23,  60,  4, 3,     "Heat Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of heat input to rated capacity(inverse of COP)"
; SAC 11/30/10 - added for DOE-2.3
        EDIT, 19275,     0, 0, 1, CHILLER,  0,       HEAT-INPUT, -1, STD, 130, 335,  23,  60,  4, 3,           "Heat Input:",  LEFT, -110, 5, 1, LEFT, 4, 5, "An alternative to HEAT-INPUT-RATIO, is the heat/fuel consumption of the chiller at the RATED conditions"
        EDIT, 18098,     0, 0, 1, CHILLER,  0,   COEF-OF-PERFOR, -1, STD, 130, 360,  23,  60,  4, 3,     "Coef of Perform.:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of rated capacity to heat consumption (inverse of HEAT-INPUT-RATIO)"
       COMBO, 19276,     0, 0, 1, CHILLER,  0,  VARIABLE-SPEED,  -1, STD, 415, 144, 120,  75, 19, 3,       "Variable Speed?",  LEFT, -130, 5, 0, LEFT, 4, 5, "Whether or not the chiller has a variable speed compressor"
    ENDCASE

    CASE, CHILLER, 0, TYPE, -1, =, 1, 8    ; CHILLER:TYPE = GAS-ABSOR 
       LABEL, "Heat/Fuel Consmp. (choose ONE):", STD, LEFT,  15, 290, 1, 0, 0, 230, 18099, 3
        EDIT, 18099, 12956, 0, 1, CHILLER,  0, HEAT-INPUT-RATIO, -1, STD, 130, 310,  23,  60,  4, 3,     "Heat Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of heat input to rated capacity(inverse of COP)"
; SAC 11/30/10 - added for DOE-2.3
        EDIT, 19274,     0, 0, 1, CHILLER,  0,       HEAT-INPUT, -1, STD, 130, 335,  23,  60,  4, 3,           "Heat Input:",  LEFT, -110, 5, 1, LEFT, 4, 5, "An alternative to HEAT-INPUT-RATIO, is the heat/fuel consumption of the chiller at the RATED conditions"
        EDIT, 18100,     0, 0, 1, CHILLER,  0,   COEF-OF-PERFOR, -1, STD, 130, 360,  23,  60,  4, 3,     "Coef of Perform.:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of rated capacity to heat consumption (inverse of HEAT-INPUT-RATIO)"
       COMBO, 19277,     0, 0, 1, CHILLER,  0,  VARIABLE-SPEED,  -1, STD, 415, 144, 120,  75, 19, 3,       "Variable Speed?",  LEFT, -130, 5, 0, LEFT, 4, 5, "Whether or not the chiller has a variable speed compressor"
    ENDCASE

    CASE, ELSE
        EDIT, 18101,     0, 0, 1, CHILLER,  0,   COEF-OF-PERFOR, -1, STD, 130, 270,  23,  60,  4, 3,     "Coef of Perform.:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of rated capacity to power (inverse of ELEC-INPUT-RATIO)"
       LABEL, "Heat/Fuel Consmp. (choose ONE):", STD, LEFT,  15, 315, 1, 0, 0, 230, 18102, 3
        EDIT, 18102, 12956, 0, 1, CHILLER,  0, HEAT-INPUT-RATIO, -1, STD, 130, 335,  23,  60,  4, 3,     "Heat Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of heat input to rated capacity(inverse of COP)"
; SAC 11/30/10 - added for DOE-2.3
        EDIT, 19273,     0, 0, 1, CHILLER,  0,       HEAT-INPUT, -1, STD, 130, 360,  23,  60,  4, 3,           "Heat Input:",  LEFT, -110, 5, 1, LEFT, 4, 5, "An alternative to HEAT-INPUT-RATIO, is the heat/fuel consumption of the chiller at the RATED conditions"

       CASE, CHILLER, 0, TYPE, -1, =, 1, 1    ; CHILLER:TYPE = OPEN-CENT
          COMBO, 19278,     0, 0, 1, CHILLER,  1,   VARIABLE-SPEED, -1, STD, 415, 144, 120,  75, 19, 3,       "Variable Speed?",  LEFT, -130, 5, 1, LEFT, 4, 5, "Specifies that a variable speed drive is installed, and the type of compressor being used (Centrifugal chillers only)"
       ENDCASE
       CASE, CHILLER, 0, TYPE, -1, =, 1, 3    ; CHILLER:TYPE = ELEC-HERM-CENT
          COMBO, 19279,     0, 0, 1, CHILLER,  3,   VARIABLE-SPEED, -1, STD, 415, 144, 120,  75, 19, 3,       "Variable Speed?",  LEFT, -130, 5, 1, LEFT, 4, 5, "Specifies that a variable speed drive is installed, and the type of compressor being used (Centrifugal chillers only)"
       ENDCASE
       CASE, ELSE
          COMBO, 19280,     0, 0, 1, CHILLER,  0,   VARIABLE-SPEED, -1, STD, 415, 144, 120,  75, 19, 3,       "Variable Speed?",  LEFT, -130, 5, 1, LEFT, 4, 5, "Specifies that a variable speed drive is installed, and the type of compressor being used (Centrifugal chillers only)"
       ENDCASE

    ENDCASE

; SAC 10/15/02 - Split out condenser keywords into separate tab
    ;******************************************
    ; Chiller - Condenser Page
    ;******************************************
    TABPAGE, 3355, 3355, 1, 3, NOTIMP, " Condenser "

; SAC 1/16/06 - Design sizing mods
       COMBO, 12963, 12875, 0, 1, CHILLER,  0,   CONDENSER-TYPE,  0, STD, 130,  10,  80, 200, 19, 3,       "Condenser Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Air Cooled=heat exchanger & condenser; Water Cooled=heat rejection & condenser loop"
        EDIT, 12957, 12957, 0, 1, CHILLER,  0,     ELEC-TO-COND, -1, STD, 130,  50,  23,  60,  2, 3,         "Elec to Cond:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Efficiency of compressor: i.e., fraction of chiller electricity input rejected to condenser, as heat"
        EDIT, 12958, 12882, 0, 1, CHILLER,  0,     HEAT-TO-COND, -1, STD, 130,  75,  23,  60,  2, 3,         "Heat to Cond:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Fraction of fuel or heat input to chiller that is rjected to condenser, as heat"
        EDIT, 12960, 12960, 0, 1, CHILLER,  0,        MAX-HTREC, -1, STD, 130, 100,  23,  60,  2, 3,       "Max Heat Recov:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Maximum fraction of design condenser heat that is available for heat recovery"
        EDIT, 18056,     0, 0, 1, CHILLER,  0,       MIN-COND-T, -1, STD, 130, 125,  23,  60,  2, 3,      "Min Condenser T:",  LEFT, -110, 5, 1, LEFT, 4, 5, "The minimum entering temperature or SCT for which operation is valid"

    LABEL, "Fan Control:", STD, LEFT, 280, 55, 1, 0, 0, 460, 18057, 3
       COMBO, 18057,     0, 0, 1, CHILLER,  0,  COND-FAN-CTRL,   -1, STD, 290,  85, 200, 170, 19, 3,          "Fan Control:",  LEFT,  0, -15, 0, LEFT, 4, 5, "The mechanism by which the fans are controlled to hold the setpoint"
       COMBO, 18058,     0, 0, 1, CHILLER,  0,  COND-PWR-FPLR,   -1, STD, 290, 125, 200, 170, 19, 3,         "Power f(PLR):",  LEFT,  0, -15, 0, LEFT, 4, 5, "The curve that modifies the fan energy as a function of the condenser part-load ratio"

    LABEL, "Remote Condenser (Air-Cooled or Evaporative):", STD, LEFT,  20, 170, 1, 0, 0, 510, 17641, 3
        EDIT, 17641,     0, 0, 1, CHILLER,  0,    COND-CAPACITY, -1, STD, 130, 190,  23,  60,  3, 3,             "Capacity:",  LEFT,  -95, 5, 1, LEFT, 4, 5, ""
        EDIT, 18059,     0, 0, 1, CHILLER,  0,     COND-FAN-PWR, -1, STD, 130, 215,  23,  60,  3, 3,            "Fan Power:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The fan power in kW; only if Capacity specified"
        EDIT, 18060,     0, 0, 1, CHILLER,  0,    COND-PUMP-PWR, -1, STD, 130, 240,  23,  60,  3, 3,           "Pump Power:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The pump power in kW; only if Capacity specified"
       LABEL, "Air-Cooled:",   STD, LEFT,  30, 272, 1, 0, 0, 250, 18061, 3
        EDIT, 18061,     0, 0, 1, CHILLER,  0,   SCT-AMBIENT-TD, -1, STD, 130, 290,  23,  60,  2, 3,         "SCT-Ambnt TD:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The differential between the SCT and the drybulb at which the condenser is rated"
        EDIT, 18062,     0, 0, 1, CHILLER,  0,  COND-FAN-EIR-TD, -1, STD, 130, 315,  23,  60,  4, 3,           "Fan EIR-TD:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "FanEIR = (Fan electric power in Btuh) / (Condenser capacity in Btuh/TD)"
        EDIT, 18063,     0, 0, 1, CHILLER,  0, REMOTE-DESIGN-DB, -1, STD, 130, 340,  23,  60,  1, 3,       "Design Drybulb:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The design drybulb temperature; default is the design-day drybulb"
       LABEL, "Water-Cooled:", STD, LEFT, 285, 197, 1, 0, 0, 510, 17642, 3
        EDIT, 17642,     0, 0, 1, CHILLER,  0,     COND-FAN-EIR, -1, STD, 420, 215,  23,  60,  4, 3,              "Fan EIR:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""
        EDIT, 17643,     0, 0, 1, CHILLER,  0,    COND-PUMP-EIR, -1, STD, 420, 240,  23,  60,  4, 3,             "Pump EIR:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""
        EDIT, 18064,     0, 0, 1, CHILLER,  0,  REMOTE-RATED-WB, -1, STD, 420, 265,  23,  60,  1, 3,      "Rated Wetbulb T:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The wetbulb at which the condenser's capacity and power are defined"
        EDIT, 18065,     0, 0, 1, CHILLER,  0, REMOTE-RATED-SCT, -1, STD, 420, 290,  23,  60,  1, 3,   "Rated Condensing T:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The SCT at which the condenser's capacity and power are defined"
        EDIT, 18066,     0, 0, 1, CHILLER,  0, REMOTE-DESIGN-WB, -1, STD, 420, 315,  23,  60,  1, 3,     "Design Wetbulb T:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The design wetbulb; default is the design-day wetbulb"
       COMBO, 18067,     0, 0, 1, CHILLER,  0,      COND-CAP-FT, -1, STD, 290, 355, 200, 220, 19, 3,  "Capacity f(SCT, WB):",  LEFT,  0, -15, 0, LEFT, 4, 5, "A curve modifying the condenser capacity as a function of the SCT and wetbulb"

    LABEL, "Temperature Control:", STD, LEFT, 510, 15, 1, 0, 0, 710, 18068, 3
       COMBO, 18068,     0, 0, 1, CHILLER,  0,  COND-SETPT-CTRL, -1, STD, 630,  35, 200,  80, 19, 3,     "Setpoint Control:",  LEFT, -110, 5, 0, LEFT, 4, 5, "May be fixed setpoint, ambient + dT setpoint, or stage fans w/ ambient"
        EDIT, 18069,     0, 0, 1, CHILLER,  0,  COND-SETPT-T,    -1, STD, 630,  60,  23,  50,  1, 3,     "Fixed Setpoint T:",  LEFT, -110, 5, 1, LEFT, 4, 5, "The fixed saturated condensing setpoint"
        EDIT, 18070,     0, 0, 1, CHILLER,  0,  COND-SETPT-DT,   -1, STD, 630,  85,  23,  50,  2, 3,     "Ambient Setpt dT:",  LEFT, -110, 5, 1, LEFT, 4, 5, "The saturated condensing temperature setpoint differential"
       COMBO, 18071,     0, 0, 1, CHILLER,  0,  AMB-FRAC-FT,     -1, STD, 520, 125, 200, 190, 19, 3,      "Ambient Staging:",  LEFT,  0, -15, 0, LEFT, 4, 5, "The curve defining the active condenser fraction as a function of the outdoor temperature"
; SAC 11/30/10 - replaced following Condenser tab w/ above (from design sizing version)
;;;       LABEL, "Condenser", STD, LEFT, 480, 175, 1, 0, 0, 675, 12963, 3
;;       COMBO, 12963, 12875, 0, 1, CHILLER,  0,   CONDENSER-TYPE,  0, STD, 570, 195,  80, 105, 19, 3,            "Cond Type:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Air Cooled=heat exchanger & condenser; Water Cooled=heat rejection & condenser loop"
;;        EDIT, 12957, 12957, 0, 1, CHILLER,  0,     ELEC-TO-COND, -1, STD, 590, 220,  23,  60,  2, 3,         "Elec to Cond:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Efficiency of compressor: i.e., fraction of chiller electricity input rejected to condenser, as heat"
;;        EDIT, 12958, 12882, 0, 1, CHILLER,  0,     HEAT-TO-COND, -1, STD, 590, 245,  23,  60,  2, 3,         "Heat to Cond:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Fraction of fuel or heat input to chiller that is rjected to condenser, as heat"
;;        EDIT, 12960, 12960, 0, 1, CHILLER,  0,        MAX-HTREC, -1, STD, 590, 270,  23,  60,  2, 3,       "Max Heat Recov:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Maximum fraction of design condenser heat that is available for heat recovery"
;;        EDIT, 17641,     0, 0, 1, CHILLER,  0,    COND-CAPACITY, -1, STD, 590, 295,  23,  60,  1, 3,             "Capacity:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
;;        EDIT, 17642,     0, 0, 1, CHILLER,  0,     COND-FAN-EIR, -1, STD, 590, 320,  23,  60,  4, 3,              "Fan EIR:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
;;        EDIT, 17643,     0, 0, 1, CHILLER,  0,    COND-PUMP-EIR, -1, STD, 590, 345,  23,  60,  4, 3,             "Pump EIR:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
;; SAC 8/18/06 - repositioned all controls and added MIN-COND-T and MAX-COND-T
;;       LABEL, "Condenser", STD, LEFT, 480, 175, 1, 0, 0, 675, 12963, 3
;       COMBO, 12963, 12875, 0, 1, CHILLER,  0,   CONDENSER-TYPE,  0, STD, 170,  45,  80, 200, 19, 3,       "Condenser Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Air Cooled=heat exchanger & condenser; Water Cooled=heat rejection & condenser loop"
;        EDIT, 12957, 12957, 0, 1, CHILLER,  0,     ELEC-TO-COND, -1, STD, 190,  70,  23,  60,  2, 3,    "Elec to Condenser:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Efficiency of compressor: i.e., fraction of chiller electricity input rejected to condenser, as heat"
;        EDIT, 12958, 12882, 0, 1, CHILLER,  0,     HEAT-TO-COND, -1, STD, 190,  95,  23,  60,  2, 3,    "Heat to Condenser:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Fraction of fuel or heat input to chiller that is rjected to condenser, as heat"
;        EDIT, 12960, 12960, 0, 1, CHILLER,  0,        MAX-HTREC, -1, STD, 190, 120,  23,  60,  2, 3,    "Max Heat Recovery:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Maximum fraction of design condenser heat that is available for heat recovery"
;        EDIT, 17641,     0, 0, 1, CHILLER,  0,    COND-CAPACITY, -1, STD, 190, 145,  23,  60,  1, 3,   "Condenser Capacity:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""
;        EDIT, 17642,     0, 0, 1, CHILLER,  0,     COND-FAN-EIR, -1, STD, 190, 170,  23,  60,  4, 3,    "Condenser Fan EIR:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""
;        EDIT, 17643,     0, 0, 1, CHILLER,  0,    COND-PUMP-EIR, -1, STD, 190, 195,  23,  60,  4, 3,   "Condenser Pump EIR:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""
;
;        EDIT, 18242,     0, 0, 1, CHILLER,  0,       MIN-COND-T, -1, STD, 430,  70,  23,  60,  1, 3,        "Min Cond Temp:",  LEFT, -105, 5, 1, LEFT, 4, 5, "the minimum allowable condensing temperature setpoint"
;        EDIT, 18243,     0, 0, 1, CHILLER,  0,       MAX-COND-T, -1, STD, 430,  95,  23,  60,  1, 3,        "Max Cond Temp:",  LEFT, -105, 5, 1, LEFT, 4, 5, "the temperature that acts as an upper limit on the leaving condenser temperature when Cond. Water Flow Control = Variable"

    ;******************************************
    ; Chiller - Performance Curves Page
    ;******************************************
    TABPAGE, 3039, 3039, 1, 3, NOTIMP, " Perf. Curves "

   LABEL, "Electric Input Ratio", STD, CENTER, 230, 5, 1, 0, 0, 0, 0, 3
   COMBO, 12967, 12967, 0, 1, CHILLER, 0,          EIR-FT,  0, STD, 150,  25, 200, 165, 19, 3,  "",  LEFT, -130, -3, 0, LEFT, 4, 5, "Quadratic Curve Fit: EIR as a function of temp of water entering condenser & leaving chilled"
   LABEL,  "f(t evap leaving,", STD, LEFT, 20, 22, 1, 0, 0, 0, 0, 3
   LABEL,  "t cond entering):", STD, LEFT, 30, 36, 1, 0, 0, 0, 0, 3
   COMBO, 12969, 12969, 0, 1, CHILLER, 0,        EIR-FPLR,  0, STD, 150,  55, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Electric Input Ratio as a function of the part load ratio"
   LABEL,  "f(part load ratio):", STD, LEFT, 20, 60, 1, 0, 0, 0, 0, 3
    
;   LABEL, "Air Condenser Power", STD, CENTER, 230, 95, 1, 0, 0, 0, 0, 3
;   COMBO, 13782, 13782, 0, 1, CHILLER, 0,    AIR-PWR-FPLR,  0, STD, 150, 115, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Quadratic Equation: condenser fan power consumption as a function of chiller capacity PLR"
;   COMBO, 13783, 13783, 0, 1, CHILLER, 0,      AIR-PWR-FT,  0, STD, 150, 145, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Quadratic Equation: condenser fan power consumption as a function of outside air drybulb"
   LABEL,    "f(part load ratio):", STD, LEFT, 20, 120, 1, 0, 0, 0, 0, 3
   LABEL,  "f(t outdoor ambient):", STD, LEFT, 20, 150, 1, 0, 0, 0, 0, 3

   LABEL, "Heat Input Ratio (HIR)", STD, CENTER, 230, 215, 1, 0, 0, 0, 13788, 3
   COMBO, 13788, 13788, 0, 1, CHILLER, 0,  GAS-HIR-FDESCT,  0, STD, 150, 235, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Quadratic Curve: Heat Input Ratio as a function of the desiccant regeneration temperature"
   LABEL,  "f(t desiccant regen):", STD, LEFT, 20, 240, 1, 0, 0, 0, 0, 3

; SAC 10/28/01 - Added new curves for HEAT-EIR-*
   LABEL, "Heating Elec Input Ratio", STD, CENTER, 230, 275, 1, 0, 0, 0, 17651, 3
   COMBO, 17651,     0, 0, 1, CHILLER, 0,      HEAT-EIR-FT,  0, STD, 150, 295, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Heating Electric Input Ratio as a function of leaving hot water and entering air temperatures (no frost on heat exchanger)"
   LABEL,  "f(t leaving HW,",       STD, LEFT, 20, 292, 1, 0, 0, 0, 0, 3
   LABEL,  "t entering air) nf:",   STD, LEFT, 30, 306, 1, 0, 0, 0, 0, 3
   COMBO, 17652,     0, 0, 1, CHILLER, 0, HEAT-EIR-FT-FRST,  0, STD, 150, 325, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Heating Electric Input Ratio as a function of leaving hot water and entering air temperatures (when frost forms on heat exchanger)"
   LABEL,  "f(t leaving HW,",       STD, LEFT, 20, 322, 1, 0, 0, 0, 0, 3
   LABEL,  "t entering air) frst:", STD, LEFT, 30, 336, 1, 0, 0, 0, 0, 3
   COMBO, 17653,     0, 0, 1, CHILLER, 0,    HEAT-EIR-FPLR,  0, STD, 150, 355, 200, 165, 19, 3,  "",  LEFT, -130,  5, 0, LEFT, 4, 5, "Heating Electric Input Ratio as a function of the heating part load ratio"
   LABEL,  "f(part load ratio):",   STD, LEFT, 20, 360, 1, 0, 0, 0, 0, 3

   LABEL,  "Heat Input Ratio", STD,  CENTER, 415, 5, 1, 0, 0, 0, 0, 3
   COMBO, 12964, 12964, 0, 1, CHILLER, 0,          HIR-FT,  0, STD, 335,  25, 200, 165, 19, 3,  "",  LEFT, -315,  5, 0, LEFT, 4, 5, "Bi-Quadratic Curve: HIR as a function of temp of entering condenser and exiting chilled water"
   COMBO, 12965, 12965, 0, 1, CHILLER, 0,        HIR-FPLR,  0, STD, 335,  55, 200, 165, 19, 3,  "",  LEFT, -315,  5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Heat Input Ratio as a function of the part load ratio"
   
   LABEL,  "Engine Heat Rejection", STD,  CENTER, 415, 95, 1, 0, 0, 0, 0, 3
   COMBO, 13784, 13784, 0, 1, CHILLER, 0,  ENG-HTREJ-FPLR,  0, STD, 335, 115, 200, 165, 19, 3,  "",  LEFT, -315,  5, 0, LEFT, 4, 5, "Quadratic Curve: amount of recoverable heat as a function of the cooling part load ratio"
   COMBO, 13785, 13785, 0, 1, CHILLER, 0,    ENG-HTREJ-FT,  0, STD, 335, 175, 200, 165, 19, 3,  "",  LEFT, -315,  5, 0, LEFT, 4, 5, "Quadratic Curve: the amount of recoverable heat as a function of the entering condenser temp"
   LABEL,  "f(t cond entering):", STD, LEFT, 20, 180, 1, 0, 0, 0, 0, 3
    
   LABEL,  "Desiccant Regen Cap", STD,  CENTER, 415, 215, 1, 0, 0, 0, 13789, 3
   COMBO, 13789, 13789, 0, 1, CHILLER, 0, GAS-QREG-FDESCT,  0, STD, 335, 235, 200, 165, 19, 3,  "",  LEFT, -315,  5, 0, LEFT, 4, 5, "Quadratic Curve: available regeneration energy as a function of the required regeneration temp"

; SAC 10/28/01 - Added new curves for HEAT-CAP-*
   LABEL, "Electric Heating Capacity", STD, CENTER, 415, 275, 1, 0, 0, 0, 17654, 3
   COMBO, 17654,     0, 0, 1, CHILLER, 0,      HEAT-CAP-FT,  0, STD, 335, 295, 200, 165, 19, 3,  "",  LEFT, -315,  5, 0, LEFT, 4, 5, "Electric Heating Capacity as a function of leaving hot water and entering air temperatures (no frost on heat exchanger)"
   COMBO, 17655,     0, 0, 1, CHILLER, 0, HEAT-CAP-FT-FRST,  0, STD, 335, 325, 200, 165, 19, 3,  "",  LEFT, -315,  5, 0, LEFT, 4, 5, "Electric Heating Capacity as a function of leaving hot water and entering air temperatures (when frost forms on heat exchanger)"
    
   LABEL, "Cooling Capacity", STD, CENTER, 600, 5, 1, 0, 0, 0, 12968, 3
   COMBO, 12968, 12968, 0, 1, CHILLER, 0,     CAPACITY-FT,  0, STD, 520,  25, 200, 165, 19, 3,  "",  LEFT, -510,  5, 0, LEFT, 4, 5, "Bi-Quadratic Curve: Capacity as function of temp of entering condenser & exiting chilled water"

   LABEL, "Gas Heating Capacity", STD, CENTER, 600, 95, 1, 0, 0, 0, 13787, 3
   COMBO, 13787, 13787, 0, 1, CHILLER, 0,  GAS-HCAP-FPLRC,  0, STD, 520, 115, 200, 165, 19, 3,  "",  LEFT, -510,  5, 0, LEFT, 4, 5, "Quadratic Curve: heating capacity as a function of the cooling part load ratio"

    ;******************************************
    ; Chiller - Attachments Page
    ;******************************************
    TABPAGE, 3040, 3040, 1, 3, NOTIMP, " Loop Attachments "

; SAC 1/16/06 - Design sizing mods - Restructured most everything
     LABEL, "Chilled Water",   STD, CENTER, 180, 10, 1, 0, 0, 0, 0, 3
     LABEL, "Condenser Water", STD, CENTER, 325, 10, 1, 0, 0, 0, 0, 3
     LABEL, "Hot Water",       STD, CENTER, 470, 10, 1, 0, 0, 0, 0, 3

     LABEL, "Series Location:",    STD, LEFT,  20,  35, 1, 0, 0, 0, 0, 3
     LABEL, "Pump:",               STD, LEFT,  20,  60, 1, 0, 0, 0, 0, 3
     LABEL, "Flow Ctrl:",          STD, LEFT,  20,  85, 1, 0, 0, 0, 0, 3
     LABEL, "Design Flow:",        STD, LEFT,  20, 110, 1, 0, 0, 0, 0, 3
     LABEL, "Design Delta T:",     STD, LEFT,  20, 135, 1, 0, 0, 0, 0, 3
     LABEL, "Head:",               STD, LEFT,  20, 160, 1, 0, 0, 0, 0, 3
     LABEL, "Static Head:",        STD, LEFT,  20, 185, 1, 0, 0, 0, 0, 3
     LABEL, "Minimum Flow:",       STD, LEFT,  20, 210, 1, 0, 0, 0, 0, 3
     LABEL, "PLR at Min Flow:",    STD, LEFT,  20, 235, 1, 0, 0, 0, 0, 3
     LABEL, "Maximum Flow:",       STD, LEFT,  20, 260, 1, 0, 0, 0, 0, 3
     LABEL, "Max leaving Temp:",   STD, LEFT,  20, 285, 1, 0, 0, 0, 0, 3
     LABEL, "Design dT, heating:", STD, LEFT,  20, 310, 1, 0, 0, 0, 0, 3

    CASE, CHILLER, 0, TYPE, -1, =, 1, 11
        ;-- Chilled Water --
        COMBO, 18035,     0, 0, 1, CHILLER, 11,   CHW-SERIES-LOCN,  0, STD, 115,  30, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "If chillers are in series, whether at the upstream or downstream location"
        COMBO, 17600, 13800, 0, 1, CHILLER, 11,          CHW-PUMP,  0, STD, 115,  55, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "Name of a Pump that serves the chiller's chilled water loop"
        COMBO, 17601, 12973, 0, 1, CHILLER, 11,     CHW-FLOW-CTRL,  0, STD, 115,  80, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "The type of flow through the chiller evaporator"
         EDIT, 17603, 12975, 0, 1, CHILLER, 11,          CHW-HEAD, -1, STD, 145, 155,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "Head loss thru the evaporator at the RATED flow"
         EDIT, 17604, 12976, 0, 1, CHILLER, 11,   CHW-STATIC-HEAD, -1, STD, 145, 180,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "The static head in the chiller circuit (typically zero)"
         EDIT, 17606, 12977, 0, 1, CHILLER, 11,      CHW-MIN-FLOW, -1, STD, 145, 205,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "Minimum allowable fraction of the design flow rate through the evaporator"
         EDIT, 17607, 13491, 0, 1, CHILLER, 11,      CHW-MAX-FLOW, -1, STD, 145, 255,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "Maximum allowable fraction of the design flow rate through the evaporator"
                                                                           
        ;-- Condenser Water --
        COMBO, 17608, 12929, 0, 1, CHILLER, 11,           CW-PUMP,  0, STD, 260,  55, 120, 135, 19, 3,                "",  LEFT, -180, 5, 0, LEFT, 4, 5,  "Name of a Pump that serves the (dedicated) evaporator recirculation loop"
        COMBO, 17609, 12980, 0, 1, CHILLER, 11,      CW-FLOW-CTRL,  0, STD, 260,  80, 120, 135, 19, 3,                "",  LEFT, -195, 5, 0, LEFT, 4, 5,  "The type of flow through the condenser"
         EDIT, 18036,     0, 0, 1, CHILLER, 10,    DESIGN-CW-FLOW, -1, STD, 290, 105,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The flow thru the condenser at DESIGN conditions; default is RATED flow"
         EDIT, 18037,     0, 0, 1, CHILLER, 10,      DESIGN-CW-DT, -1, STD, 290, 130,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The condenser temperature rise at DESIGN conditions; default is RATED flow"
         EDIT, 17611, 12982, 0, 1, CHILLER, 11,           CW-HEAD, -1, STD, 290, 155,  23,  55,  1, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "Head loss thru the condenser at the RATED flow"
         EDIT, 17612, 12983, 0, 1, CHILLER, 11,    CW-STATIC-HEAD, -1, STD, 290, 180,  23,  55,  1, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "Static pressure drop through the condenser at the design flow rate"
         EDIT, 17614, 12984, 0, 1, CHILLER, 11,       CW-MIN-FLOW, -1, STD, 290, 205,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "Minimum allowable flow rate through the condenser (as a fraction of the design flow rate)"
         EDIT, 18038,     0, 0, 1, CHILLER, 10,        CW-MIN-PLR, -1, STD, 290, 230,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The part-load ratio corresponding to the minimum flow"
         EDIT, 18039,     0, 0, 1, CHILLER, 10,        MAX-COND-T, -1, STD, 290, 280,  23,  55,  1, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "When variable flow, the maximum allowable leaving temperature"
         EDIT, 18040,     0, 0, 1, CHILLER, 10,   DESIGN-CW-DT-HT, -1, STD, 290, 305,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The condenser temperature drop at heating DESIGN conditions; default is RATED heating flow"
                                                                           
        ;-- Hot Water --
        COMBO, 18041,     0, 0, 1, CHILLER, 10,    HW-SERIES-LOCN,  0, STD, 405,  30, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "For a chiller/heater in series, whether at the upstream or downstream location"
        COMBO, 17615, 12991, 0, 1, CHILLER, 11,           HW-PUMP,  0, STD, 405,  55, 120, 135, 19, 3,                "",  LEFT, -315, 5, 0, LEFT, 4, 5,  ""
        COMBO, 17616, 12992, 0, 1, CHILLER, 11,      HW-FLOW-CTRL,  0, STD, 405,  80, 120, 135, 19, 3,                "",  LEFT, -330, 5, 0, LEFT, 4, 5,  "Constant Flow = independent of the load; Variable Flow = varies linearly with load"
         EDIT, 17618, 12994, 0, 1, CHILLER, 11,           HW-HEAD, -1, STD, 435, 155,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Head loss thru the condenser at the RATED flow"
         EDIT, 17619, 12995, 0, 1, CHILLER, 11,    HW-STATIC-HEAD, -1, STD, 435, 180,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Static HW pressure drop through the chiller; use if pumping fluid at atm pressure into loop"
         EDIT, 17621, 12996, 0, 1, CHILLER, 11,       HW-MIN-FLOW, -1, STD, 435, 205,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Min hot water flow rate through chiller; used only if Hot Water Flow Control = Variable Flow"
         EDIT, 17622, 13492, 0, 1, CHILLER, 11,       HW-MAX-FLOW, -1, STD, 435, 255,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Max hot water flow rate through chiller; used only if Hot Water Flow Control = Variable Flow"
      
;        LABEL, "Well Water", STD, CENTER, 615, 10, 1, 0, 0, 0, 0, 3
;        COMBO, 17623,     0, 0, 1, CHILLER, 11,         WELL-PUMP,  0, STD, 550,  55, 120, 135, 19, 3,                "",  LEFT, -450, 5, 0, LEFT, 4, 5,  "Name of the well pump attached directly to the condenser heat-exchanger"
;        COMBO, 17624,     0, 0, 1, CHILLER, 11,    WELL-FLOW-CTRL,  0, STD, 550,  80, 120, 135, 19, 3,                "",  LEFT, -465, 5, 0, LEFT, 4, 5,  "Flow may be either constant (3-way valve) or variable (two-way valve)"
;         EDIT, 17625,     0, 0, 1, CHILLER, 11,     RATED-WELL-DT, -1, STD, 580, 130,  23,  55,  2, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "The temperature rise through the well-side of the condenser-to-well heat-exchanger at the rated conditions"
;         EDIT, 17626,     0, 0, 1, CHILLER, 11,      WELL-HX-HEAD, -1, STD, 580, 155,  23,  55,  1, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Head loss thru the condenser-to-well heat-exchanger at the RATED flow"
;         EDIT, 17627,     0, 0, 1, CHILLER, 11,  WELL-STATIC-HEAD, -1, STD, 580, 180,  23,  55,  1, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Static head may be specified here, or in the Well Loop (but not normally both)"
;         EDIT, 17629,     0, 0, 1, CHILLER, 11,     WELL-MIN-FLOW, -1, STD, 580, 205,  23,  55,  2, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "The minimum allowable well-water flow through the heat exchangers"

    ENDCASE

; SAC 10/28/01 - Added CASE statements by Chiller Type to accomodate differences in SubType compatibility for CHW-LOOP, HW-LOOP & CW-LOOP assignments -AND- for varying CONDENSER-TYPE symbol types
    CASE, CHILLER, 0, TYPE, -1, =, 1, 10
        ;-- Chilled Water --
        COMBO, 18042,     0, 0, 1, CHILLER, 10,   CHW-SERIES-LOCN,  0, STD, 115,  30, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "If chillers are in series, whether at the upstream or downstream location"
        COMBO, 17565, 13800, 0, 1, CHILLER, 10,          CHW-PUMP,  0, STD, 115,  55, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "Name of a Pump that serves the chiller's chilled water loop"
        COMBO, 17566, 12973, 0, 1, CHILLER, 10,     CHW-FLOW-CTRL,  0, STD, 115,  80, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "The type of flow through the chiller evaporator"
         EDIT, 17568, 12975, 0, 1, CHILLER, 10,          CHW-HEAD, -1, STD, 145, 155,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "Head loss thru the evaporator at the RATED flow"
         EDIT, 17569, 12976, 0, 1, CHILLER, 10,   CHW-STATIC-HEAD, -1, STD, 145, 180,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "The static head in the chiller circuit (typically zero)"
         EDIT, 17571, 12977, 0, 1, CHILLER, 10,      CHW-MIN-FLOW, -1, STD, 145, 205,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "Minimum allowable fraction of the design flow rate through the evaporator"
         EDIT, 17572, 13491, 0, 1, CHILLER, 10,      CHW-MAX-FLOW, -1, STD, 145, 255,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "Maximum allowable fraction of the design flow rate through the evaporator"
                                                                           
        ;-- Condenser Water --
        COMBO, 17573, 12929, 0, 1, CHILLER, 10,           CW-PUMP,  0, STD, 260,  55, 120, 135, 19, 3,                "",  LEFT, -180, 5, 0, LEFT, 4, 5,  "Name of a Pump that serves the (dedicated) evaporator recirculation loop"
        COMBO, 17574, 12980, 0, 1, CHILLER, 10,      CW-FLOW-CTRL,  0, STD, 260,  80, 120, 135, 19, 3,                "",  LEFT, -195, 5, 0, LEFT, 4, 5,  "The type of flow through the condenser"
         EDIT, 18043,     0, 0, 1, CHILLER, 10,    DESIGN-CW-FLOW, -1, STD, 290, 105,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The flow thru the condenser at DESIGN conditions; default is RATED flow"
         EDIT, 18044,     0, 0, 1, CHILLER, 10,      DESIGN-CW-DT, -1, STD, 290, 130,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The condenser temperature rise at DESIGN conditions; default is RATED flow"
         EDIT, 17576, 12982, 0, 1, CHILLER, 10,           CW-HEAD, -1, STD, 290, 155,  23,  55,  1, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "Head loss thru the condenser at the RATED flow"
         EDIT, 17577, 12983, 0, 1, CHILLER, 10,    CW-STATIC-HEAD, -1, STD, 290, 180,  23,  55,  1, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "Static pressure drop through the condenser at the design flow rate"
         EDIT, 17579, 12984, 0, 1, CHILLER, 10,       CW-MIN-FLOW, -1, STD, 290, 205,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "Minimum allowable flow rate through the condenser (as a fraction of the design flow rate)"
         EDIT, 18045,     0, 0, 1, CHILLER, 10,        CW-MIN-PLR, -1, STD, 290, 230,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The part-load ratio corresponding to the minimum flow"
         EDIT, 18046,     0, 0, 1, CHILLER, 10,        MAX-COND-T, -1, STD, 290, 280,  23,  55,  1, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "When variable flow, the maximum allowable leaving temperature"
         EDIT, 18047,     0, 0, 1, CHILLER, 10,   DESIGN-CW-DT-HT, -1, STD, 290, 305,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The condenser temperature drop at heating DESIGN conditions; default is RATED heating flow"
                                                                           
        ;-- Hot Water --
        COMBO, 18048,     0, 0, 1, CHILLER, 10,    HW-SERIES-LOCN,  0, STD, 405,  30, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "For a chiller/heater in series, whether at the upstream or downstream location"
        COMBO, 17580, 12991, 0, 1, CHILLER, 10,           HW-PUMP,  0, STD, 405,  55, 120, 135, 19, 3,                "",  LEFT, -315, 5, 0, LEFT, 4, 5,  ""
        COMBO, 17581, 12992, 0, 1, CHILLER, 10,      HW-FLOW-CTRL,  0, STD, 405,  80, 120, 135, 19, 3,                "",  LEFT, -330, 5, 0, LEFT, 4, 5,  "Constant Flow = independent of the load; Variable Flow = varies linearly with load"
         EDIT, 17583, 12994, 0, 1, CHILLER, 10,           HW-HEAD, -1, STD, 435, 155,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Head loss thru the condenser at the RATED flow"
         EDIT, 17584, 12995, 0, 1, CHILLER, 10,    HW-STATIC-HEAD, -1, STD, 435, 180,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Static HW pressure drop through the chiller; use if pumping fluid at atm pressure into loop"
         EDIT, 17586, 12996, 0, 1, CHILLER, 10,       HW-MIN-FLOW, -1, STD, 435, 205,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Min hot water flow rate through chiller; used only if Hot Water Flow Control = Variable Flow"
         EDIT, 17587, 13492, 0, 1, CHILLER, 10,       HW-MAX-FLOW, -1, STD, 435, 255,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Max hot water flow rate through chiller; used only if Hot Water Flow Control = Variable Flow"
      
        LABEL, "Heat Recovery", STD, CENTER, 615, 10, 1, 0, 0, 0, 0, 3
        COMBO, 17588, 12998, 0, 1, CHILLER, 10,        HTREC-PUMP,  0, STD, 550,  55, 120, 135, 19, 3,                "",  LEFT, -450, 5, 0, LEFT, 4, 5,  "Name of pump dedicated to provide chiller's Heat Recovery Head and Heat Rec. Static Head"
        COMBO, 17589, 12999, 0, 1, CHILLER, 10,   HTREC-FLOW-CTRL,  0, STD, 550,  80, 120, 135, 19, 3,                "",  LEFT, -465, 5, 0, LEFT, 4, 5,  "The type of heat recovery water flow through the chiller"
         EDIT, 17590, 13005, 0, 1, CHILLER, 10,          HTREC-DT, -1, STD, 580, 130,  23,  55,  2, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Temperature rise of water flowing through the heat-recovery condenser, at design conditions"
         EDIT, 17591, 13001, 0, 1, CHILLER, 10,        HTREC-HEAD, -1, STD, 580, 155,  23,  55,  1, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Head loss thru the heat-recovery condenser at the design flow"
         EDIT, 17592, 13002, 0, 1, CHILLER, 10, HTREC-STATIC-HEAD, -1, STD, 580, 180,  23,  55,  1, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Static pressure drop through the heat recovery heat exchanger"
         EDIT, 17594, 13003, 0, 1, CHILLER, 10,    HTREC-MIN-FLOW, -1, STD, 580, 205,  23,  55,  2, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Minimum allowable flow rate through the heat-recovery condenser"
         EDIT, 17595, 13531, 0, 1, CHILLER, 10,     MAX-RECOVER-T, -1, STD, 580, 280,  23,  55,  1, 3,                "",  LEFT, -565, 5, 1, LEFT, 4, 5,  "Maximum temperature at which heat can be recovered from the chiller"
    ENDCASE
   
    CASE, ELSE
        ;-- Chilled Water --
        COMBO, 18049,     0, 0, 1, CHILLER,  0,   CHW-SERIES-LOCN,  0, STD, 115,  30, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "If chillers are in series, whether at the upstream or downstream location"
        COMBO, 12972, 13800, 0, 1, CHILLER,  0,          CHW-PUMP,  0, STD, 115,  55, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "Name of a Pump that serves the chiller's chilled water loop"
        COMBO, 12973, 12973, 0, 1, CHILLER,  0,     CHW-FLOW-CTRL,  0, STD, 115,  80, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "The type of flow through the chiller evaporator"
         EDIT, 12975, 12975, 0, 1, CHILLER,  0,          CHW-HEAD, -1, STD, 145, 155,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "Head loss thru the evaporator at the RATED flow"
         EDIT, 12976, 12976, 0, 1, CHILLER,  0,   CHW-STATIC-HEAD, -1, STD, 145, 180,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "The static head in the chiller circuit (typically zero)"
         EDIT, 12977, 12977, 0, 1, CHILLER,  0,      CHW-MIN-FLOW, -1, STD, 145, 205,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "Minimum allowable fraction of the design flow rate through the evaporator"
         EDIT, 13491, 13491, 0, 1, CHILLER,  0,      CHW-MAX-FLOW, -1, STD, 145, 255,  23,  55,  1, 3,                "",  LEFT, -115, 5, 1, LEFT, 4, 5,  "Maximum allowable fraction of the design flow rate through the evaporator"
                                                                           
        ;-- Condenser Water --
        COMBO, 12979, 12929, 0, 1, CHILLER,  0,           CW-PUMP,  0, STD, 260,  55, 120, 135, 19, 3,                "",  LEFT, -180, 5, 0, LEFT, 4, 5,  "Name of a Pump that serves the (dedicated) evaporator recirculation loop"
        COMBO, 12980, 12980, 0, 1, CHILLER,  0,      CW-FLOW-CTRL,  0, STD, 260,  80, 120, 135, 19, 3,                "",  LEFT, -195, 5, 0, LEFT, 4, 5,  "The type of flow through the condenser"
         EDIT, 18050,     0, 0, 1, CHILLER,  0,    DESIGN-CW-FLOW, -1, STD, 290, 105,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The flow thru the condenser at DESIGN conditions; default is RATED flow"
         EDIT, 18051,     0, 0, 1, CHILLER,  0,      DESIGN-CW-DT, -1, STD, 290, 130,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The condenser temperature rise at DESIGN conditions; default is RATED flow"
         EDIT, 12982, 12982, 0, 1, CHILLER,  0,           CW-HEAD, -1, STD, 290, 155,  23,  55,  1, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "Head loss thru the condenser at the RATED flow"
         EDIT, 12983, 12983, 0, 1, CHILLER,  0,    CW-STATIC-HEAD, -1, STD, 290, 180,  23,  55,  1, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "Static pressure drop through the condenser at the design flow rate"
         EDIT, 12984, 12984, 0, 1, CHILLER,  0,       CW-MIN-FLOW, -1, STD, 290, 205,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "Minimum allowable flow rate through the condenser (as a fraction of the design flow rate)"
         EDIT, 18052,     0, 0, 1, CHILLER,  0,        CW-MIN-PLR, -1, STD, 290, 230,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The part-load ratio corresponding to the minimum flow"
         EDIT, 18053,     0, 0, 1, CHILLER,  0,        MAX-COND-T, -1, STD, 290, 280,  23,  55,  1, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "When variable flow, the maximum allowable leaving temperature"
         EDIT, 18054,     0, 0, 1, CHILLER,  0,   DESIGN-CW-DT-HT, -1, STD, 290, 305,  23,  55,  2, 3,                "",  LEFT, -250, 5, 1, LEFT, 4, 5,  "The condenser temperature drop at heating DESIGN conditions; default is RATED heating flow"
                                                                           
        ;-- Hot Water --
        COMBO, 18055,     0, 0, 1, CHILLER,  0,    HW-SERIES-LOCN,  0, STD, 405,  30, 120, 135, 19, 3,                "",  LEFT,  -70, 5, 0, LEFT, 4, 5,  "For a chiller/heater in series, whether at the upstream or downstream location"
        COMBO, 12991, 12991, 0, 1, CHILLER,  0,           HW-PUMP,  0, STD, 405,  55, 120, 135, 19, 3,                "",  LEFT, -315, 5, 0, LEFT, 4, 5,  ""
        COMBO, 12992, 12992, 0, 1, CHILLER,  0,      HW-FLOW-CTRL,  0, STD, 405,  80, 120, 135, 19, 3,                "",  LEFT, -330, 5, 0, LEFT, 4, 5,  "Constant Flow = independent of the load; Variable Flow = varies linearly with load"
         EDIT, 12994, 12994, 0, 1, CHILLER,  0,           HW-HEAD, -1, STD, 435, 155,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Head loss thru the condenser at the RATED flow"
         EDIT, 12995, 12995, 0, 1, CHILLER,  0,    HW-STATIC-HEAD, -1, STD, 435, 180,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Static HW pressure drop through the chiller; use if pumping fluid at atm pressure into loop"
         EDIT, 12996, 12996, 0, 1, CHILLER,  0,       HW-MIN-FLOW, -1, STD, 435, 205,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Min hot water flow rate through chiller; used only if Hot Water Flow Control = Variable Flow"
         EDIT, 13492, 13492, 0, 1, CHILLER,  0,       HW-MAX-FLOW, -1, STD, 435, 255,  23,  55,  1, 3,                "",  LEFT, -375, 5, 1, LEFT, 4, 5,  "Max hot water flow rate through chiller; used only if Hot Water Flow Control = Variable Flow"
      
        LABEL, "Heat Recovery", STD, CENTER, 615, 10, 1, 0, 0, 0, 0, 3
        COMBO, 12998, 12998, 0, 1, CHILLER,  0,        HTREC-PUMP,  0, STD, 550,  55, 120, 135, 19, 3,                "",  LEFT, -450, 5, 0, LEFT, 4, 5,  "Name of pump dedicated to provide chiller's Heat Recovery Head and Heat Rec. Static Head"
        COMBO, 12999, 12999, 0, 1, CHILLER,  0,   HTREC-FLOW-CTRL,  0, STD, 550,  80, 120, 135, 19, 3,                "",  LEFT, -465, 5, 0, LEFT, 4, 5,  "The type of heat recovery water flow through the chiller"
         EDIT, 13005, 13005, 0, 1, CHILLER,  0,          HTREC-DT, -1, STD, 580, 130,  23,  55,  2, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Temperature rise of water flowing through the heat-recovery condenser, at design conditions"
         EDIT, 13001, 13001, 0, 1, CHILLER,  0,        HTREC-HEAD, -1, STD, 580, 155,  23,  55,  1, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Head loss thru the heat-recovery condenser at the design flow"
         EDIT, 13002, 13002, 0, 1, CHILLER,  0, HTREC-STATIC-HEAD, -1, STD, 580, 180,  23,  55,  1, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Static pressure drop through the heat recovery heat exchanger"
         EDIT, 13003, 13003, 0, 1, CHILLER,  0,    HTREC-MIN-FLOW, -1, STD, 580, 205,  23,  55,  2, 3,                "",  LEFT, -530, 5, 1, LEFT, 4, 5,  "Minimum allowable flow rate through the heat-recovery condenser"
         EDIT, 13531, 13531, 0, 1, CHILLER,  0,     MAX-RECOVER-T, -1, STD, 580, 280,  23,  55,  1, 3,                "",  LEFT, -565, 5, 1, LEFT, 4, 5,  "Maximum temperature at which heat can be recovered from the chiller"
    ENDCASE

    ;******************************************
    ; Chiller - Miscellaneous Page
    ;******************************************
    TABPAGE, 3041, 2023, 1, 3, NOTIMP, " Miscellaneous "

   LABEL, "Auxiliaries", STD, LEFT, 20, 15, 1, 0, 0, 240, 12986, 3
    EDIT, 12986, 13795, 0, 1, CHILLER, 0,           AUX-KW, -1, STD, 160,  35,  23,  60,  1, 3,               "Power:", LEFT, -125, 5, 1, LEFT, 4, 5, "Auxiliary electric power consumption of the chiller"
   COMBO, 12988, 12988, 0, 1, CHILLER, 0,     AUX-SCHEDULE,  0, STD, 100,  60, 120, 140, 19, 3,            "Schedule:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Schedule for Auxiliary Power consumption (set Auxiliary Mode to Scheduled to activate this)"
   COMBO, 12987, 12987, 0, 1, CHILLER, 0,         AUX-MODE,  0, STD, 100,  85, 120, 140, 19, 3,                "Mode:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Always=all hours;When On=If chiller on;When Off=if chiller off;Scheduled=use Aux Schedule"
   COMBO, 12989, 12989, 0, 1, CHILLER, 0,        AUX-METER,  0, STD, 100, 110, 120, 140, 19, 3,               "Meter:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption of this chiller's auxiliaries"
    
   LABEL, "Absorption Cooling", STD, LEFT, 20, 155, 1, 0, 0, 240, 13778, 3
;    EDIT, 13650, 13650, 0, 1, CHILLER, 0, SOLUTION-PUMP-KW, -1, STD, 160, 175,  23,  60,  1, 3,    "Solution Pump kW:", LEFT, -125, 5, 1, LEFT, 4, 5, "Electricity consumption of the solution pump"
    EDIT, 13778, 13778, 0, 1, CHILLER, 0,  GAS-COMB-FAN-KW, -1, STD, 160, 175,  23,  60,  1, 3,   "Combustion Fan kW:", LEFT, -125, 5, 1, LEFT, 4, 5, "Electricity consumption of the combustion blower"
;   EDIT, 13779, 13779, 0, 1, CHILLER, 0,   GAS-HCAP-RATIO, -1, STD, 160, 200,  23,  60,  1, 3, "Heat/Cool Cap Ratio:", LEFT, -125, 5, 1, LEFT, 4, 5, "Ratio of the design heating capacity to the design cooling capacity"
    EDIT, 13780, 13780, 0, 1, CHILLER, 0,      GAS-HW-XEFF, -1, STD, 160, 200,  23,  60,  1, 3,  "Heating Efficiency:", LEFT, -125, 5, 1, LEFT, 4, 5, "The burner efficiency (when the chiller is in the heating mode)"
    EDIT, 13781, 13781, 0, 1, CHILLER, 0,    GAS-DESC-XEFF, -1, STD, 160, 225,  23,  60,  1, 3, "Desiccant Regen Eff:", LEFT, -125, 5, 1, LEFT, 4, 5, "The burner efficiency when regenerating a desiccant system"

   LABEL, "Engine-Driven Chiller", STD, LEFT, 20, 300, 1, 0, 0, 240, 13534, 3
    EDIT, 13534, 13848, 0, 1, CHILLER, 0,  ENG-HEAT-TO-JAC, -1, STD, 160, 320,  23,  60,  2, 3,      "Heat-To-Jacket:", LEFT, -125, 5, 1, LEFT, 4, 5, "Fraction of design fuel consumption that is recoverable from the jacket of an engine-chiller"
    EDIT, 13643, 13849, 0, 1, CHILLER, 0,  ENG-HEAT-TO-EXH, -1, STD, 160, 345,  23,  60,  2, 3,     "Heat-To-Exhaust:", LEFT, -125, 5, 1, LEFT, 4, 5, "Fraction of design fuel consumption that is recoverable from the exhaust of an engine-chiller"

; SAC 1/16/06 - Design sizing mods + Updated RATED-WSE-TD & MIN-WSE-TD control labels
   LABEL, "Free Cooling", STD, LEFT, 310, 15, 1, 0, 0, 580, 18026, 3
    EDIT, 18026,     0, 0, 1, CHILLER, 0, THERMOCYCLE-CAP,  -1, STD, 470,  35,  23,  60,  2, 3,  "Thermocycle Capacity:", LEFT, -140, 5, 1, LEFT, 4, 5, "The fraction of rated capacity available in the thermocycle mode"
    EDIT, 18027,     0, 0, 1, CHILLER, 0, RATED-WSE-TD,     -1, STD, 470,  60,  23,  60,  1, 3,          "Rated WSE TD:", LEFT, -140, 5, 1, LEFT, 4, 5, "The rated temperature differential between entering chw and cw flows"
    EDIT, 18028,     0, 0, 1, CHILLER, 0, MIN-WSE-TD,       -1, STD, 470,  85,  23,  60,  1, 3,        "Minimum WSE TD:", LEFT, -140, 5, 1, LEFT, 4, 5, "The minimum differential necessary to enable the waterside economizer"

   LABEL, "Heat Exchangers (counterflow)", STD, LEFT, 310, 155, 1, 0, 0, 695, 17656, 3
   LABEL, "Evaporator", STD, CENTER, 535, 170, 1, 0, 0, 0, 17656, 3
    EDIT, 17656,     0, 0, 1, CHILLER, 0,       EVAP-HX-TD, -1, STD, 505, 187,  23,  60,  2, 3,     "Design Temp. Differential:", LEFT, -175, 5, 0, LEFT, 4, 5, ""
    EDIT, 17657,     0, 0, 1, CHILLER, 0,  EVAP-HX-SETPT-T, -1, STD, 505, 212,  23,  60,  2, 3,          "Setpoint Temperature:", LEFT, -175, 5, 0, LEFT, 4, 5, ""
   LABEL, "Condenser",  STD, CENTER, 610, 170, 1, 0, 0, 0, 17658, 3
    EDIT, 17658,     0, 0, 1, CHILLER, 0,       COND-HX-TD, -1, STD, 580, 187,  23,  60,  2, 3,                               "", LEFT,   -1, 5, 1, LEFT, 4, 5, ""
    EDIT, 17659,     0, 0, 1, CHILLER, 0,  COND-HX-SETPT-T, -1, STD, 580, 212,  23,  60,  2, 3,                               "", LEFT,   -1, 5, 1, LEFT, 4, 5, ""

; SAC 1/16/06 - Design sizing mods
   LABEL, "Well-Water Exchangers, Loop-to-Loop Heat Pump", STD, LEFT, 310, 263, 1, 0, 0, 695, 18029, 3
   LABEL, "Evaporator", STD, CENTER, 535, 278, 1, 0, 0, 0, 17656, 3
    EDIT, 18029,     0, 0, 1, CHILLER, 0, EVAP-HX-TD,       -1, STD, 505, 295,  23,  60,  3, 3,  "Design HX Temp. Differential:", LEFT, -175, 5, 0, LEFT, 4, 5, "The design temperature differential between the entering chilled-water and well-water streams"
    EDIT, 18030,     0, 0, 1, CHILLER, 0, EVAP-HX-UA,       -1, STD, 505, 320,  23,  60,  1, 3,             "Heat-Exchanger UA:", LEFT, -175, 5, 0, LEFT, 4, 5, "The UA product of the evaporator-to-well heat exchanger; alternative to 'Design Temperature Differential'"
    EDIT, 18031,     0, 0, 1, CHILLER, 0, EVAP-HX-SETPT-T,  -1, STD, 505, 345,  23,  60,  2, 3,       "HX Setpoint Temperature:", LEFT, -175, 5, 0, LEFT, 4, 5, "When heating only, specifies the temperature setpoint of the chilled-water leaving the evaporator"
   LABEL, "Condenser",  STD, CENTER, 610, 278, 1, 0, 0, 0, 17658, 3
    EDIT, 18032,     0, 0, 1, CHILLER, 0, COND-HX-TD,       -1, STD, 580, 295,  23,  60,  3, 3,                               "", LEFT, -170, 5, 1, LEFT, 4, 5, "The design temperature differential between the entering condenser-water and well-water streams"
    EDIT, 18033,     0, 0, 1, CHILLER, 0, COND-HX-UA,       -1, STD, 580, 320,  23,  60,  1, 3,                               "", LEFT, -170, 5, 1, LEFT, 4, 5, "The UA product of the condenser-to-well heat exchanger; alternative to 'Design Temperature Differential'"
    EDIT, 18034,     0, 0, 1, CHILLER, 0, COND-HX-SETPT-T,  -1, STD, 580, 345,  23,  60,  2, 3,                               "", LEFT, -170, 5, 1, LEFT, 4, 5, "When cooling only, specifies the temperature setpoint of the condenser-water leaving the heat-exchanger"

; SAC 11/30/10 - replaced old Misc tab (below) w/ one from design sizing UI (above) - w/ some adjustments
;   LABEL, "Start-up and Shut-down Times", STD, LEFT, 40, 25, 1, 0, 0, 255, 13644, 3
;    EDIT, 13644, 13644, 0, 1, CHILLER, 0,    START-UP-TIME, -1, STD, 185,  45,  23,  50,  3, 3,       "Start-up Time:", LEFT, -125, 5, 1, LEFT, 4, 5, "Equivalent full-load time required to start up the chiller (in hours or fraction of hours)"
;    EDIT, 17890, 13644, 0, 1, CHILLER, 0,    STANDBY-TIME,  -1, STD, 185,  70,  23,  50,  3, 3,        "Standby Time:", LEFT, -125, 5, 1, LEFT, 4, 5, "Equivalent full-load time required to keep the chiller on-line with no load (in hours or fraction of hours)"
;    EDIT, 13649, 13649, 0, 1, CHILLER, 0,   SHUT-DOWN-TIME, -1, STD, 185,  95,  23,  50,  3, 3,           "Shut-down:", LEFT, -125, 5, 1, LEFT, 4, 5, "Equivalent full-load time required to shut down the chiller (in hours or fraction of hours)"
;   
;   LABEL, "Absorption Cooling", STD, LEFT, 40, 125, 1, 0, 0, 255, 13650, 3
;;    EDIT, 13650, 13650, 0, 1, CHILLER, 0, SOLUTION-PUMP-KW, -1, STD, 185, 145,  23,  50,  1, 3,    "Solution Pump kW:", LEFT, -125, 5, 1, LEFT, 4, 5, "Electricity consumption of the solution pump"   ; SAC 11/24/10 - removed
;    EDIT, 13778, 13778, 0, 1, CHILLER, 0,  GAS-COMB-FAN-KW, -1, STD, 185, 170,  23,  50,  1, 3,   "Combustion Fan kW:", LEFT, -125, 5, 1, LEFT, 4, 5, "Electricity consumption of the combustion blower"
;;   EDIT, 13779, 13779, 0, 1, CHILLER, 0,   GAS-HCAP-RATIO, -1, STD, 185, 195,  23,  50,  1, 3, "Heat/Cool Cap Ratio:", LEFT, -125, 5, 1, LEFT, 4, 5, "Ratio of the design heating capacity to the design cooling capacity"
;    EDIT, 13780, 13780, 0, 1, CHILLER, 0,      GAS-HW-XEFF, -1, STD, 185, 195,  23,  50,  1, 3,  "Heating Efficiency:", LEFT, -125, 5, 1, LEFT, 4, 5, "The burner efficiency (when the chiller is in the heating mode)"
;    EDIT, 13781, 13781, 0, 1, CHILLER, 0,    GAS-DESC-XEFF, -1, STD, 185, 220,  23,  50,  1, 3, "Desiccant Regen Eff:", LEFT, -125, 5, 1, LEFT, 4, 5, "The burner efficiency when regenerating a desiccant system"
;   
;   LABEL, "Auxiliaries", STD, LEFT, 370, 25, 1, 0, 0, 580, 12986, 3
;    EDIT, 12986, 13795, 0, 1, CHILLER, 0,           AUX-KW, -1, STD, 510,  45,  23,  50,  1, 3,               "Power:", LEFT, -120, 5, 1, LEFT, 4, 5, "Auxiliary electric power consumption of the chiller"
;   COMBO, 12988, 12988, 0, 1, CHILLER, 0,     AUX-SCHEDULE,  0, STD, 455,  70, 120, 125, 19, 3,            "Schedule:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Schedule for Auxiliary Power consumption (set Auxiliary Mode to Scheduled to activate this)"
;   COMBO, 12987, 12987, 0, 1, CHILLER, 0,         AUX-MODE,  0, STD, 455,  95, 120, 125, 19, 3,                "Mode:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Always=all hours;When On=If chiller on;When Off=if chiller off;Scheduled=use Aux Schedule"
;   COMBO, 12989, 12989, 0, 1, CHILLER, 0,        AUX-METER,  0, STD, 455, 120, 120, 125, 19, 3,               "Meter:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption of this chiller's auxiliaries"
;    
;   LABEL, "Engine-Driven Chiller", STD, LEFT, 370, 175, 1, 0, 0, 580, 13534, 3
;    EDIT, 13534, 13848, 0, 1, CHILLER, 0,  ENG-HEAT-TO-JAC, -1, STD, 510, 195,  23,  50,  2, 3,      "Heat-To-Jacket:", LEFT, -120, 5, 1, LEFT, 4, 5, "Fraction of design fuel consumption that is recoverable from the jacket of an engine-chiller"
;    EDIT, 13643, 13849, 0, 1, CHILLER, 0,  ENG-HEAT-TO-EXH, -1, STD, 510, 220,  23,  50,  2, 3,     "Heat-To-Exhaust:", LEFT, -120, 5, 1, LEFT, 4, 5, "Fraction of design fuel consumption that is recoverable from the exhaust of an engine-chiller"
;
;   LABEL, "Heat Exchangers (counterflow)", STD, LEFT, 190, 275, 1, 0, 0, 580, 17658, 3
;   LABEL, "Evaporator", STD, CENTER, 445, 291, 1, 0, 0, 0, 17656, 3
;    EDIT, 17656,     0, 0, 1, CHILLER, 0,       EVAP-HX-TD, -1, STD, 415, 310,  23,  60,  2, 3,  "Design Temperature Differential:", LEFT, -205, 5, 1, LEFT, 4, 5, ""
;    EDIT, 17657,     0, 0, 1, CHILLER, 0,  EVAP-HX-SETPT-T, -1, STD, 415, 335,  23,  60,  2, 3,             "Setpoint Temperature:", LEFT, -205, 5, 1, LEFT, 4, 5, ""
;   LABEL, "Condenser",  STD, CENTER, 530, 291, 1, 0, 0, 0, 17658, 3
;    EDIT, 17658,     0, 0, 1, CHILLER, 0,       COND-HX-TD, -1, STD, 500, 310,  23,  60,  2, 3,                                  "", LEFT,   -1, 5, 1, LEFT, 4, 5, ""
;    EDIT, 17659,     0, 0, 1, CHILLER, 0,  COND-HX-SETPT-T, -1, STD, 500, 335,  23,  60,  2, 3,                                  "", LEFT,   -1, 5, 1, LEFT, 4, 5, ""

    ;******************************************
    ; Chiller - Compliance Page
    ;******************************************
; AFR 7/21/09 - removed    
;    TABPAGE, 3351, 3351, 1, 1, NOTIMP, " Compliance "

; SAC 10/24/00 - added compliance inputs
;   LABEL, "Compliance Inputs",   STD, LEFT, 20, 300, 0, 0, 1, 435, 15498, 1
; AFR 7/21/09 - moved to the Basic Specifications tab
;   COMBO, 15500,     0, 0, 1, CHILLER, 0,           C-TYPE,  0, STD, 220,  45, 300, 105, 19, 1, "Chiller Type:",                     LEFT, -190,  5, 0, LEFT, 4, 5, "The type of chiller"
; AFR 7/21/09 - moved to the Basic Specifications tab
;    EDIT, 15498,     0, 0, 1, CHILLER, 0,   C-NUM-OF-UNITS, -1, STD, 220,  70,  23,  90,  0, 1, "Number of Chillers:",               LEFT, -190,  5, 1, LEFT, 4, 5, "The total number of chillers simulated as one unit"
;   EDIT, 15499,     0, 0, 1, CHILLER, 0,  C-TOTAL-CLG-CAP, -1, STD, 220,  70,  23,  90,  1, 1, "Total Capacity:",                   LEFT, -190,  5, 1, LEFT, 4, 5, "The total capacity of all chillers simulated as one unit"

; SAC 7/25/06 - removed per KJM e-mail of 6/27/06
;    EDIT, 17510,     0, 0, 1, CHILLER, 0,     C-DESIGN-CAP, -1, STD, 220,  95,  23,  90,  0, 1, "Capacity at Design Conditions:",    LEFT, -190,  5, 1, LEFT, 4, 5, "Chiler Capacity at design chilled and condenser water tempreatures"
;    EDIT, 17511,     0, 0, 1, CHILLER, 0,    C-TOT-DSN-CAP, -1, STD, 220, 120,  23,  90,  0, 1, "Total Capacity of All Chillers:",   LEFT, -190,  5, 1, LEFT, 4, 5, "Total Capacity at design chilled and condenser water temps for all chillers simulated as one"
;    EDIT, 17512,     0, 0, 1, CHILLER, 0,   C-DESIGN-CHW-T, -1, STD, 220, 145,  23,  90,  2, 1, "Design Chilled Water Temp:",        LEFT, -190,  5, 1, LEFT, 4, 5, "Design leaving chilled water loop temperature"
;    EDIT, 17513,     0, 0, 1, CHILLER, 0,  C-DESIGN-COND-T, -1, STD, 220, 170,  23,  90,  2, 1, "Design Condenser Water Temp:",      LEFT, -190,  5, 1, LEFT, 4, 5, "Design entering consenser water loop temperature"

; AFR 7/21/09 - moved to the Basic Specifications tab
;    EDIT, 15501,     0, 0, 1, CHILLER, 0,            C-COP, -1, STD, 440,  45,  23,  60,  2, 1, "COP:",                   LEFT,  -35,  5, 1, LEFT, 4, 5, "The coefficient of performance of this chiller"
;    EDIT, 15502,     0, 0, 1, CHILLER, 0,           C-IPLV, -1, STD, 440,  70,  23,  60,  2, 1, "IPLV:",                  LEFT,  -35,  5, 1, LEFT, 4, 5, "The integrated part load value of this chiller"




 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Boiler - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODTABDLG, 3029, 10201, 1, 100, 100, 310, 600, 0, "Boiler Type:  ", BOILER, 0, TYPE, 0, 0, 0, "     Boiler Name:  ", BOILER, 0, NAME, 0, 0, 0, ""
MODTABDLG, 3029, 10201, 1, 100, 100, 470, 750, 0, BOILER, "Boiler Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 12791, 12791, 0, 1, BOILER, 0, NAME,  0, STD, 205,  15, 400, 250, 19, 3, "Currently Active Boiler:", RIGHT, -8, 5, 0, LEFT, 4, 5, "List of all boilers defined in project; also allows library retrieval and creation"
   STATIC, 1, BOILER, 0, TYPE, 0, 0, 0, 475, 20, 300, STD, LEFT, "Type: ",   "", 0, 3

    ;******************************************
    ; Boiler - Basic Specifications Page
    ;******************************************
    TABPAGE, 3030, 3030, 1, 3, NOTIMP, " Basic Specifications "
    
    EDIT, 12899, 12899, 0, 1, BOILER,  0,             NAME,  0, STD,  95,   0,  23, 250, 32, 3,  "Boiler Name:", RIGHT,   -8, 5, 0, LEFT, 4, 5, "Name of the boiler; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 12873, 12873, 0, 1, BOILER,  0,             TYPE,  0, STD,  95,  25, 300, 130, 19, 3,          "Type:",  RIGHT,  -8, 5, 0, LEFT, 4, 5, "Can be fuel or electric, hot water or steam, and with or without draft fans"
;  COMBO, 19154, 12792, 0, 1, BOILER, 0,              TYPE,  0, STD,  70,  10, 300, 140, 19, 3,                 "Type:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Can be fuel or electric, hot water or steam, and with or without draft fans"
    
   LABEL,  "Loop Assignments", STD, LEFT, 20, 55, 1, 0, 0, 210, 19130, 3
   COMBO, 19130, 19129, 0, 1, BOILER, 0,          HW-LOOP,  0, STD,  70,  75, 200, 140, 19, 3,                   "HW:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of the loop that the boiler serves (Loop Type must be Hot Water, Two Pipe, or WLHP)"
    
   LABEL, "Meter Assignments", STD, LEFT, 20, 130, 1, 0, 0, 210, 0, 3
   COMBO, 12089, 12809, 0, 1, BOILER, 0,       FUEL-METER,  0, STD, 105, 150, 120, 105, 19, 3,           "Fuel Meter:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Name of the Fuel Meter that tallies the fuel consumption of this boiler"
   COMBO, 12094, 12810, 0, 1, BOILER, 0,       ELEC-METER,  0, STD, 105, 175, 120, 105, 19, 3,       "Electric Meter:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption of this boiler"
   
;  COMBO, 12071, 12795, 0, 1, BOILER, 0,        COST-DATA,  0, STD,  60, 225, 120, 140, 19, 3,                 "Cost:",  LEFT,  -40, 5, 0, LEFT, 4, 5, ""

; SAC 10/24/00 - added compliance inputs
   LABEL, "Compliance Inputs",   STD, LEFT, 20, 230, 0, 0, 1, 230, 15505, 1
    EDIT, 15505,     0, 0, 1, BOILER, 0,   C-NUM-OF-UNITS, -1, STD, 130, 250,  23,  70,  0, 1, "Number of Boilers:",     LEFT, -110, 5, 1, LEFT, 4, 5, "The total number of boilers simulated as one unit"
;   EDIT, 15506,     0, 0, 1, BOILER, 0,  C-TOTAL-HTG-CAP, -1, STD, 110, 275,  23,  90,  1, 1, "Total Capacity:",        LEFT,  -90, 5, 1, LEFT, 4, 5, "The total capacity of all boilers simulated as one unit"
    EDIT, 15507,     0, 0, 1, BOILER, 0,           C-AFUE, -1, STD, 130, 275,  23,  70,  2, 1, "AFUE:",                  LEFT, -110, 5, 1, LEFT, 4, 5, "The AFUE of this boiler"
    EDIT, 15508,     0, 0, 1, BOILER, 0,  C-THERM-EFF-MAX, -1, STD, 130, 300,  23,  70,  2, 1, "Therm Eff @ Max:",       LEFT, -110, 5, 1, LEFT, 4, 5, "The thermal efficiency of this boiler at its maximum output capacity"

; SAC 7/13/04 - changed decimal precision from 1->3 & increased size of each control
   LABEL, "Equipment Capacity", STD, LEFT, 270, 55, 1, 0, 0, 465, 0, 3
    EDIT, 12135, 12796, 0, 1, BOILER, 0,         CAPACITY, -1, STD, 335,  75,  23,  85,  3, 3,             "Capacity:",  LEFT,  -65, 5, 1, LEFT, 4, 5, "Nominal (rated) heating capacity of the boiler (in millions of BTU's per hour)"
    EDIT, 12136, 12797, 0, 1, BOILER, 0,   CAPACITY-RATIO, -1, STD, 365, 100,  23,  55,  2, 3,       "Capacity Ratio:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Capacity as fraction of max heating load (used only if DOE-2 sizes the boiler)"
    EDIT, 12141, 12141, 0, 1, BOILER, 0,        MIN-RATIO, -1, STD, 365, 125,  23,  55,  2, 3,            "Min Ratio:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Minimum boiler operating ratio (a fraction of the Capacity); below this, it cycles on & off"
    EDIT, 12145, 12145, 0, 1, BOILER, 0,        MAX-RATIO, -1, STD, 365, 150,  23,  55,  2, 3,            "Max Ratio:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Maximum allowable boiler operating ratio (a fraction of the Capacity)"
   
   LABEL, "Equipment Efficiency", STD, LEFT, 520, 55, 1, 0, 0, 720, 0, 3
    EDIT, 12151, 12798, 0, 1, BOILER, 0, HEAT-INPUT-RATIO, -1, STD, 625,  75,  23,  65,  3, 3,     "Heat Input Ratio:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Dimensionless ratio of fuel heat input to boiler output at full load (at rated conditions)"
    EDIT, 12155, 12799, 0, 1, BOILER, 0, ELEC-INPUT-RATIO, -1, STD, 625, 100,  23,  65,  4, 3,     "Elec Input Ratio:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to nominal capacity (at rated conditions)"
    EDIT, 18975, 18975, 0, 1, BOILER, 0,      RATED-HWR-T, -1, STD, 635, 125,  23,  55,  1, 3,    "Return Water Tmp.:",  LEFT, -115, 5, 1, LEFT, 4, 5, "specifies the return water temperature at which both the CAPACITY and HEAT-INPUT-RATIO are defined (for HW-CONDENSING boilers)"
   
   COMBO, 12758, 12758, 0, 1, BOILER, 0,         LOCATION,  0, STD, 595, 170, 300, 125, 19, 3,             "Location:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Outdoors=heat lost to environment; Zone=heat lost to the Boiler Zone"
   COMBO, 13000, 12087, 0, 1, BOILER, 0,        ZONE-NAME,  0, STD, 595, 195, 300, 125, 19, 3,          "Boiler Zone:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Name of zone that the boiler is in (receives heat lost from tank)"
    EDIT, 13111, 13186, 0, 1, BOILER, 0, AQUASTAT-SETPT-T, -1, STD, 640, 220,  23,  60,  2, 3,  "Aquastat Setpoint T:",  LEFT, -125, 5, 1, LEFT, 4, 5, "The setpoint of the boiler's internal aquastat"

; SAC 11/30/10 - added for DOE-2.3
   LABEL, "Design vs. Rated Conditions", STD, LEFT, 445, 262, 1, 0, 0, 720, 0, 3
   LABEL, "Design", STD, CENTER, 598, 277, 1, 0, 0, 0, 18026, 3
    EDIT, 18026,     0, 0, 1, BOILER, 0, DESIGN-HW-T,      -1, STD, 570, 295,  23,  55,  1, 3,       "Hot-Water Temp:",  LEFT, -117, 5, 1, LEFT, 4, 5, "Leaving hot-water temperature at the DESIGN conditions; default is loop setpoint"
    EDIT, 18027,     0, 0, 1, BOILER, 0, DESIGN-AMBIENT-T, -1, STD, 570, 320,  23,  55,  1, 3,     "Ambient Air Temp:",  LEFT, -117, 5, 1, LEFT, 4, 5, "Ambient temperature at the DESIGN conditions, default is design-day"
    EDIT, 19283,     0, 0, 1, BOILER, 0, DESIGN-HWR-T,     -1, STD, 570, 345,  23,  55,  1, 3,   "Hot Water Return T:",  LEFT, -117, 5, 1, LEFT, 4, 5, "For HW-CONDENSING, the design return temperature. Default is the return temperature of the loop"
   LABEL, "Rated",  STD, CENTER, 678, 277, 1, 0, 0, 0, 18028, 3
    EDIT, 18028,     0, 0, 1, BOILER, 0, RATED-HW-T,       -1, STD, 650, 295,  23,  55,  1, 3,                      "",  LEFT,    0, 5, 1, LEFT, 4, 5, "Leaving hot-water temperature at the RATED conditions"
    EDIT, 18029,     0, 0, 1, BOILER, 0, RATED-AMBIENT-T,  -1, STD, 650, 320,  23,  55,  1, 3,                      "",  LEFT,    0, 5, 1, LEFT, 4, 5, "Ambient temperature at the RATED conditions"
    
    ;******************************************
    ; Boiler - Performance Curves Page
    ;******************************************
    TABPAGE, 3031, 3031, 1, 3, NOTIMP, " Performance Curves "
    
   LABEL,  "f(part load ratio):", STD, LEFT, 20, 45, 1, 0, 0, 0, 0, 3
   LABEL,  "f(t water entering,", STD, LEFT, 20, 74, 1, 0, 0, 0, 0, 3
   LABEL,  "t water leaving):",   STD, LEFT, 30, 87, 1, 0, 0, 0, 0, 3

   LABEL,  "Heat Input Ratio", STD, CENTER, 230, 25, 1, 0, 0, 0, 0, 3
   COMBO, 12172, 12172, 0, 1, BOILER, 0,    HIR-FPLR,  0, STD, 150,  45, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Heat Input Ratio as a function of the part load ratio"
   COMBO, 12174, 12174, 0, 1, BOILER, 0,      HIR-FT,  0, STD, 150,  80, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Bi-Quadratic Curve: the HIR as a function of the temp of entering and exiting water"
    
   LABEL, "Electric Input Ratio", STD, CENTER, 415, 25, 1, 0, 0, 0, 12175, 3
   COMBO, 12175, 12175, 0, 1, BOILER, 0,    EIR-FPLR,  0, STD, 335,  45, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Electric Input Ratio as a function of the part load ratio"
; SAC 11/30/10 - added for DOE-2.3
   COMBO, 18025,     0, 0, 1, BOILER, 0,      EIR-FT,  0, STD, 335,  80, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "The electric input ratio as a function of leaving HW temperature and ambient temperature"
   
   LABEL, "Capacity", STD, CENTER, 600, 25, 1, 0, 0, 0, 12176, 3
   COMBO, 12176, 12176, 0, 1, BOILER, 0, CAPACITY-FT,  0, STD, 520,  80, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Bi-Quadratic Curve: Capacity as a function of the temp of entering and exiting water"
    
    ;******************************************
    ; Boiler - Attachments Page
    ;******************************************
    TABPAGE, 3032, 3032, 1, 3, NOTIMP, " Loop Attachments "
    
;   LABEL, "Recirculation Loops:", ITALIC_UND, LEFT, 10, 20, 1, 0, 0, 3
   LABEL, "Hot Water", STD, CENTER, 155, 30, 1, 0, 0, 0, 0, 3
; SAC 11/30/10 - added for DOE-2.3
   COMBO, 17884,     0, 0, 1, BOILER, 0, HW-SERIES-LOCN,  0, STD, 120,  50, 200, 110, 19, 3,  "Series Location:",  LEFT, -100, 5, 0, LEFT, 4, 5, "For a boiler in series, whether at the upstream or downstream location"
   COMBO, 12179, 12897, 0, 1, BOILER, 0,        HW-PUMP,  0, STD,  75,  75, 200, 155, 19, 3,             "Pump:",  LEFT,  -55, 5, 0, LEFT, 4, 5, "Hot Water pump: if not specified, the head requirement is passed to the primary loop"
   COMBO, 12180, 12180, 0, 1, BOILER, 0,   HW-FLOW-CTRL,  0, STD, 120, 100,  80, 110, 19, 3,     "Flow Control:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Constant Flow = independent of the load; Variable Flow = varies linearly with load"
; SAC 11/30/10 - added for DOE-2.3
;    EDIT, 12182, 12182, 0, 1, BOILER, 0,          HW-DT, -1, STD, 135, 125,  23,  45,  1, 3,          "Delta T:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Design temp change of hot water through the boiler (used to size recirculation pump, if present)"
    EDIT, 18024,     0, 0, 1, BOILER, 0,    RATED-HW-DT, -1, STD, 135, 125,  23,  45,  2, 3, "Rated HW Delta-T:",  LEFT, -115, 5, 1, LEFT, 4, 5, "The RATED temperature rise corresponding to the Head"
    EDIT, 12184, 12184, 0, 1, BOILER, 0,        HW-HEAD, -1, STD, 135, 150,  23,  45,  1, 3,             "Head:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Pressure drop through the boiler at the design flowrate"
    EDIT, 12186, 12186, 0, 1, BOILER, 0, HW-STATIC-HEAD, -1, STD, 135, 175,  23,  45,  1, 3,      "Static Head:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Static pressure drop through the boiler; use if pumping fluid at atm pressure into loop"
    EDIT, 12187, 12187, 0, 1, BOILER, 0,    HW-MIN-FLOW, -1, STD, 135, 200,  23,  45,  1, 3,     "Minimum Flow:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Min flow rate through the boiler; used only if Hot Water Flow Control = Variable Flow"
    EDIT, 12121, 12121, 0, 1, BOILER, 0,    HW-MAX-FLOW, -1, STD, 135, 225,  23,  45,  1, 3,     "Maximum Flow:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Max flow rate through the boiler; used only if Hot Water Flow Control = Variable Flow"
; SDG 3/20/13 Hybrid GLHP 
    EDIT, 18103, 18103, 0, 1, BOILER, 0, HW-BYPASS-FLOW, -1, STD, 135, 250,  23,  45,  1, 3,      "Bypass Flow:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Fraction of the total loop flow that will be conditioned by the boiler, but that is bypassed around the boiler"
;  COMBO, 12188, 12188, 0, 1, BOILER, 0,   HW-ISOLATION,  0, STD, 135, 250,  80,  57, 19, 3,        "Isolation:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Whether the boiler has an isolation valve that closes when the boiler is not being used"

    ;******************************************
    ; Boiler - Miscellaneous Page
    ;******************************************
    TABPAGE, 3117, 2024, 1, 3, NOTIMP, " Miscellaneous "
    
   LABEL, "Start-up Time", STD, LEFT, 40, 25, 1, 0, 0, 255, 12036, 3
    EDIT, 12036,   684, 0, 1, BOILER, 0,  START-UP-TIME, -1, STD, 185,  45,  23,  50,  3, 3, "Start-up Time:", LEFT, -125, 5, 1, LEFT, 4, 5, "Equivalent full-load time (in hours) required to bring the boiler on-line"
    EDIT, 17889,   684, 0, 1, BOILER, 0,  STANDBY-TIME,  -1, STD, 185,  70,  23,  50,  3, 3,  "Standby Time:", LEFT, -125, 5, 1, LEFT, 4, 5, "Equivalent full-load time (in hours) required to Keep the boiler on-line with no load"
   
   LABEL, "Auxiliaries", STD, LEFT, 370, 25, 1, 0, 0, 580, 12197, 3
    EDIT, 12197, 12807, 0, 1, BOILER, 0,         AUX-KW, -1, STD, 510,  45,  23,  50,  1, 3,     "Power:", LEFT, -120, 5, 1, LEFT, 4, 5, "Auxiliary electric power consumption of the boiler (e.g., control panels)"
   COMBO, 12198, 12198, 0, 1, BOILER, 0,       AUX-MODE,  0, STD, 455,  70, 120, 125, 19, 3,  "Schedule:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Always=all hours;When On=If boiler on;When Off=if boiler off;Scheduled=use Aux Schedule"
   COMBO, 12199, 12199, 0, 1, BOILER, 0,   AUX-SCHEDULE,  0, STD, 455,  95, 120, 125, 19, 3,      "Mode:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Schedule for Auxiliary Power consumption (set Auxiliary Mode to Scheduled to activate this)"
   COMBO, 12200, 12200, 0, 1, BOILER, 0,      AUX-METER,  0, STD, 455, 120, 120, 125, 19, 3,     "Meter:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption of this boiler's auxiliaries"
   

    
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Domestic Water Heater - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODTABDLG, 3091, 32067, 1, 100, 100, 310, 600, 0, "Hot Water Heater Type:  ", DW-HEATER, 0, TYPE, 0, 0, 0, "     Hot Water Heater Name:  ", DW-HEATER, 0, NAME, 0, 0, 0, ""
 MODTABDLG, 3091, 32067, 1, 100, 100, 550, 760, 0, DW-HEATER, "Domestic Water Heater Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 12735, 12735, 0, 1, DW-HEATER, 0, NAME,  0, STD, 260,  15, 400, 250, 19, 3, "Currently Active Water Heater:", RIGHT, -8, 5, 0, LEFT, 4, 5, "List of all domestic water heaters defined in project; also allows library retrieval and creation"
   STATIC, 1, DW-HEATER, 0, TYPE, 0, 0, 0, 530, 20, 300, STD, LEFT, "Type: ",   "", 0, 3

    ;******************************************
    ; Domestic Water Heater - Basic Specifications Page
    ;******************************************
    TABPAGE, 3092, 32067, 1, 3, NOTIMP, " Basic Specifications "
   
    EDIT, 12399, 12735, 0, 1, DW-HEATER, 0,             NAME,  0, STD, 140,  10,  23, 200, 32, 3,      "DHW Heater Name:", RIGHT,   -8, 5, 0, LEFT, 4, 5, "Name of the domestic water heater; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 12736, 13187, 0, 1, DW-HEATER, 0,             TYPE,  0, STD, 415,  10, 300, 100, 19, 3,                 "Type:", RIGHT,   -8, 5, 0, LEFT, 4, 5, "Type of DHW heater: gas, electric or heat pump"

   LABEL,  "Loop Assignments", STD, LEFT, 20, 55, 1, 0, 0, 220, 19132, 3
   COMBO, 19132,   800, 0, 1, DW-HEATER, 0,         DHW-LOOP,  0, STD,  65,  75, 200, 155, 19, 3,                  "DHW:",  LEFT,  -45, 5, 0, LEFT, 4, 5, "Name of the Domestic Hot Water loop that this heater serves"
    
   LABEL, "Meter Assignments", STD, LEFT, 20, 130, 1, 0, 0, 220, 0, 3
   COMBO, 13136,   808, 0, 1, DW-HEATER, 0,       FUEL-METER,  0, STD, 115, 150, 120, 105, 19, 3,           "Fuel Meter:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "Name of the Fuel Meter that tallies the fuel consumption of this DHW heater"
   COMBO, 13138,   809, 0, 1, DW-HEATER, 0,       ELEC-METER,  0, STD, 115, 175, 120, 105, 19, 3,       "Electric Meter:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption of this DHW heater"
   
;  COMBO, 12072, 12072, 0, 1, DW-HEATER, 0,        COST-DATA,  0, STD,  70, 200, 120, 140, 19, 3,                 "Cost:",  LEFT,  -50, 5, 0, LEFT, 4, 5, ""
   
; SAC 10/24/00 - added compliance inputs
   LABEL, "Compliance Inputs",   STD, LEFT, 20, 310, 0, 0, 1, 445, 15505, 1
   COMBO, 15510,     0, 0, 1, DW-HEATER, 0,           C-TYPE,  0, STD,  85, 330, 200, 120, 19, 1, "Type:",              LEFT,  -65, 5, 0, LEFT, 4, 5, "The type of this water heater"
   COMBO, 15511,     0, 0, 1, DW-HEATER, 0,       C-CATEGORY,  0, STD,  85, 355, 200, 120, 19, 1, "Category:",          LEFT,  -65, 5, 0, LEFT, 4, 5, "The category of this water heater"
    EDIT, 15512,     0, 0, 1, DW-HEATER, 0,   C-NUM-OF-UNITS, -1, STD, 115, 380,  23,  60,  0, 1, "Number of Htrs:",    LEFT,  -95, 5, 1, LEFT, 4, 5, "The total number of water heaters simulated as one"
    EDIT, 15513,     0, 0, 1, DW-HEATER, 0,      C-RECOV-EFF, -1, STD, 115, 405,  23,  60,  3, 1, "Recovery Eff:",      LEFT,  -95, 5, 1, LEFT, 4, 5, "The recovery efficiency of this water heater"
    EDIT, 15514,     0, 0, 1, DW-HEATER, 0,  C-ENERGY-FACTOR, -1, STD, 115, 430,  23,  60,  3, 1, "Energy Factor:",     LEFT,  -95, 5, 1, LEFT, 4, 5, "The energy factor of this water"

    EDIT, 15518,     0, 0, 1, DW-HEATER, 0,     C-PILOT-BTUH, -1, STD, 315, 355,  23,  60,  2, 1, "Pilot Energy:",      LEFT,  -95, 5, 1, LEFT, 4, 5, "The fuel consumption rate of the pilot light for this water heater"
    EDIT, 15515,     0, 0, 1, DW-HEATER, 0, C-STBY-LOSS-FRAC, -1, STD, 315, 380,  23,  60,  3, 1, "Standby Loss:",      LEFT,  -95, 5, 1, LEFT, 4, 5, "The hourly standby loss fraction for this water heater"
    EDIT, 15516,     0, 0, 1, DW-HEATER, 0,  C-TANK-INT-RVAL, -1, STD, 315, 405,  23,  60,  2, 1, "Tank Int R-val:",    LEFT,  -95, 5, 1, LEFT, 4, 5, "The R-Value of the internal tank insulation of this water heater"
    EDIT, 15517,     0, 0, 1, DW-HEATER, 0,  C-TANK-EXT-RVAL, -1, STD, 315, 430,  23,  60,  2, 1, "Tank Ext R-val:",    LEFT,  -95, 5, 1, LEFT, 4, 5, "The R-Value of the external tank insulation of this water heater"

   LABEL, "Equipment Capacity", STD, LEFT, 275, 55, 1, 0, 0, 455, 13139, 3
    EDIT, 13139,   802, 0, 1, DW-HEATER, 0,         CAPACITY, -1, STD, 340,  75,  23,  75,  3, 3,             "Capacity:",  LEFT,  -65, 5, 1, LEFT, 4, 5, "Nominal (rated) heating capacity of the water heater (in millions of BTU's per hour)"
    EDIT, 13184,   803, 0, 1, DW-HEATER, 0,   CAPACITY-RATIO, -1, STD, 370, 100,  23,  45,  2, 3,       "Capacity Ratio:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Capacity as fraction of max heating load (used only if DOE-2 sizes the water heater)"
    EDIT, 13185, 13185, 0, 1, DW-HEATER, 0, HP-SUPP-CAPACITY, -1, STD, 370, 125,  23,  45,  2, 3,          "HP Supp Cap:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "The capacity of the backup immersion heater"
   
   LABEL, "Equipment Efficiency", STD, LEFT, 510, 55, 1, 0, 0, 735, 0, 3
    EDIT, 13187,   804, 0, 1, DW-HEATER, 0, HEAT-INPUT-RATIO, -1, STD, 615,  75,  23,  65,  2, 3,     "Heat Input Ratio:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Dimensionless ratio of fuel heat input to DHW heater output at full load (at rated conditions)"
    EDIT, 13188,   805, 0, 1, DW-HEATER, 0, ELEC-INPUT-RATIO, -1, STD, 615, 100,  23,  65,  4, 3,     "Elec Input Ratio:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to nominal capacity (at rated conditions)"

; SAC 11/30/10 - added for DOE-2.3
   LABEL, "Design vs. Rated Conditions", STD, LEFT, 482, 152, 1, 0, 0, 735, 0, 3
   LABEL, "Design", STD, CENTER, 620, 167, 1, 0, 0, 0, 18019, 3
    EDIT, 18019,     0, 0, 1, DW-HEATER, 0, DESIGN-DHW-T,     -1, STD, 595, 185,  23,  50,  1, 3,          "Supply Temp:",  LEFT, -113, 5, 1, LEFT, 3, 5, "Leaving water temperature at the DESIGN conditions; default is loop setpoint"
    EDIT, 18020,     0, 0, 1, DW-HEATER, 0, DESIGN-AMBIENT-T, -1, STD, 595, 210,  23,  50,  1, 3,     "Ambient Air Temp:",  LEFT, -113, 5, 1, LEFT, 3, 5, "Ambient temperature at the DESIGN conditions, default is design-day"
    EDIT, 18021,     0, 0, 1, DW-HEATER, 0, DESIGN-HP-MIN-T,  -1, STD, 595, 235,  23,  50,  1, 3,       "Min HP Ambient:",  LEFT, -113, 5, 1, LEFT, 3, 5, "The minimum allowable ambient temperature to be used in sizing a heat-pump water heater"
   LABEL, "Rated",  STD, CENTER, 695, 167, 1, 0, 0, 0, 18022, 3
    EDIT, 18022,     0, 0, 1, DW-HEATER, 0, RATED-DHW-T,      -1, STD, 670, 185,  23,  50,  1, 3,                      "",  LEFT,    0, 5, 1, LEFT, 3, 5, "Leaving water temperature at the RATED conditions"
    EDIT, 18023,     0, 0, 1, DW-HEATER, 0, RATED-AMBIENT-T,  -1, STD, 670, 210,  23,  50,  1, 3,                      "",  LEFT,    0, 5, 1, LEFT, 3, 5, "Ambient temperature at the RATED conditions"

   LABEL, "Tank", STD, LEFT, 510, 285, 1, 0, 0, 735, 13189, 3
    EDIT, 13189, 13189, 0, 1, DW-HEATER, 0,      TANK-VOLUME, -1, STD, 615, 305,  23,  65,  2, 3,          "Tank Volume:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Volume of the DHW storage tank"
    EDIT, 13190, 12757, 0, 1, DW-HEATER, 0,          TANK-UA, -1, STD, 615, 330,  23,  65,  2, 3,              "Tank UA:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Thermal conductivity of the DHW storage tank"
   COMBO, 13191,   801, 0, 1, DW-HEATER, 0,         LOCATION,  0, STD, 585, 355, 200, 140, 19, 3,             "Location:",  LEFT,  -75, 5, 0, LEFT, 4, 5, "For DHW storage tank: Outdoors=heat lost to environment; Zone=heat lost to the DHW Zone"
   COMBO, 13192, 12755, 0, 1, DW-HEATER, 0,        ZONE-NAME,  0, STD, 585, 380, 200, 140, 19, 3,             "DHW Zone:",  LEFT,  -75, 5, 0, LEFT, 4, 5, "Name of zone that the DHW storage tank is in (receives heat lost from tank)"
    EDIT, 13194, 13194, 0, 1, DW-HEATER, 0,    MAX-HP-TANK-T, -1, STD, 615, 405,  23,  65,  2, 3,        "Max HP Tank T:",  LEFT, -105, 5, 1, LEFT, 4, 5, "The maximum water temperature that the heat pump can provide"
; SAC 11/30/10 - added for DOE-2.3
    EDIT, 18018,   808, 0, 1, DW-HEATER, 0, AQUASTAT-SETPT-T, -1, STD, 615, 430,  23,  65,  2, 3,     "Aquastat Setpt T:",  LEFT, -105, 5, 1, LEFT, 4, 5, "The setpoint of the heater's internal aquastat"
   
    ;******************************************
    ; Domestic Water Heater - Performance Curves Page
    ;******************************************
    TABPAGE, 3093, 32067, 1, 3, NOTIMP, " Performance Curves "
    
   LABEL,  "f(part load ratio):", STD, LEFT, 20, 50, 1, 0, 0, 0, 0, 3
   LABEL,  "f(t water entering,", STD, LEFT, 20, 74, 1, 0, 0, 0, 0, 3
   LABEL,  "t water leaving):",   STD, LEFT, 30, 89, 1, 0, 0, 0, 0, 3

   LABEL,  "Heat Input Ratio", STD, CENTER, 230, 25, 1, 0, 0, 0, 0, 3
   COMBO, 13195, 13195, 0, 1, DW-HEATER, 0,    HIR-FPLR,  0, STD, 150,  45, 200, 165, 19, 3, "",  LEFT, -5, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Heat Input Ratio as a function of the part load ratio"
   COMBO, 13197, 13197, 0, 1, DW-HEATER, 0,      HIR-FT,  0, STD, 150,  80, 200, 165, 19, 3, "",  LEFT, -5, 5, 0, LEFT, 4, 5, "Bi-Quadratic Curve: the HIR as a function of the temp of entering and exiting water"
    
   LABEL, "Electric Input Ratio", STD, CENTER, 415, 25, 1, 0, 0, 0, 0, 3
   COMBO, 13198, 13198, 0, 1, DW-HEATER, 0,    EIR-FPLR,  0, STD, 335,  45, 200, 165, 19, 3, "",  LEFT, -5, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Electric Input Ratio as a function of the part load ratio"
   COMBO, 13199, 13199, 0, 1, DW-HEATER, 0,      EIR-FT,  0, STD, 335,  80, 200, 165, 19, 3, "",  LEFT, -5, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Electric Input Ratio as a function of temperature entering & leaving water"
   
   LABEL, "Capacity", STD, CENTER, 600, 25, 1, 0, 0, 0, 13201, 3
   COMBO, 13201, 13201, 0, 1, DW-HEATER, 0, CAPACITY-FT,  0, STD, 520,  80, 200, 165, 19, 3, "",  LEFT, -5, 5, 0, LEFT, 4, 5, "Bi-Quadratic Curve: Capacity as a function of the temp of entering and exiting water"
    
    ;******************************************
    ; Domestic Water Heater - Attachments Page
    ;******************************************
    TABPAGE, 3094, 32067, 1, 3, NOTIMP, " Attachments "
    
   LABEL, "Domestic Hot Water", STD, CENTER, 175, 35, 1, 0, 0, 0, 13242, 3
; SAC 11/30/10 - added for DOE-2.3
   COMBO, 18017,     0, 0, 1, DW-HEATER, 0,  DHW-SERIES-LOCN,  0, STD, 120,  55, 200, 110, 19, 3,  "Series Location:",  LEFT, -100, 5, 0, LEFT, 4, 5, "For a heater in series, whether at the upstream or downstream location"
; SAC 11/30/10 - added for DOE-2.3
;   COMBO, 13242, 12751, 0, 1, DW-HEATER, 0,         DHW-PUMP,  0, STD,  75,  55, 200, 140, 19, 3,         "Pump:",  LEFT,  -55, 5, 0, LEFT, 4, 5, "Hot Water pump: if not specified, the head requirement is passed to the primary loop"
    EDIT, 13204, 12752, 0, 1, DW-HEATER, 0,         DHW-HEAD, -1, STD, 120,  80,  23,  45,  1, 3,         "Head:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Pressure drop through the DHW heater at the design flowrate"
    EDIT, 13205, 12756, 0, 1, DW-HEATER, 0,  DHW-STATIC-HEAD, -1, STD, 120, 105,  23,  45,  1, 3,  "Static Head:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Static pressure drop through the heater; use if pumping fluid at atm pressure into loop"
; SAC 11/30/10 - added for DOE-2.3
;    EDIT, 13206, 13206, 0, 1, DW-HEATER, 0,      DW-MIN-FLOW, -1, STD, 120, 130,  23,  45,  1, 3, "Minimum Flow:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Minimum flow rate through the DHW heater"
    EDIT, 13207, 13207, 0, 1, DW-HEATER, 0,     DHW-MAX-FLOW, -1, STD, 120, 155,  23,  45,  1, 3, "Maximum Flow:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Maximum flow rate through the DHW heater"
    
    ;******************************************
    ; Domestic Water Heater - Miscellaneous Page
    ;******************************************
    TABPAGE, 3118, 32067, 1, 3, NOTIMP, " Miscellaneous "
 
   LABEL, "Auxiliaries", STD, LEFT, 370, 25, 1, 0, 0, 580, 13208, 3
    EDIT, 13208,   806, 0, 1, DW-HEATER, 0,          AUX-KW, -1, STD, 510,  45,  23,  50,  1, 3,    "Power:", LEFT, -120, 5, 1, LEFT, 4, 5, "Auxiliary electric power consumption of the DHW water heater (e.g., control panels)"
   COMBO, 13209, 13209, 0, 1, DW-HEATER, 0,        AUX-MODE,  0, STD, 455,  70, 120, 125, 19, 3,     "Mode:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Always=all hours;When On=If heater on;When Off=if heater off;Scheduled=use Aux Schedule"
   COMBO, 13210, 13210, 0, 1, DW-HEATER, 0,    AUX-SCHEDULE,  0, STD, 455,  95, 120, 125, 19, 3, "Schedule:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Schedule for Auxiliary Power consumption (set Auxiliary Mode to Scheduled to activate this)"
   COMBO, 13241, 13241, 0, 1, DW-HEATER, 0,       AUX-METER,  0, STD, 455, 120, 120, 125, 19, 3,    "Meter:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption of this heater's auxiliaries"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Heat Rejection - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODTABDLG, 3033, 32068, 1, 100, 100, 310, 600, 0, "Heat Rejection Type:  ", HEAT-REJECTION, 0, TYPE, 0, 0, 0, "     Heat Rejection Name:  ", HEAT-REJECTION, 0, NAME, 0, 0, 0, ""
 MODTABDLG, 3033, 32068, 1, 100, 100, 500, 710, 0, HEAT-REJECTION, "Heat Rejection Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 12189, 12899, 0, 1, HEAT-REJECTION, 0, NAME,  0, STD, 240,  15, 400, 250, 19, 3, "Currently Active Heat Rejection:", RIGHT, -8, 5, 0, LEFT, 4, 5, "List of all heat rejection components defined in project; also allows library retrieval and creation"
   STATIC, 1, HEAT-REJECTION, 0, TYPE, 0, 0, 0, 510, 20, 300, STD, LEFT, "Type: ",   "", 0, 3

  ;******************************************
  ; Heat Rejection - Basic Specifications Page
  ;******************************************
  TABPAGE, 3034, 32068, 1, 3, NOTIMP, " Basic Specifications "
    
    EDIT, 12899, 12899, 0, 1, HEAT-REJECTION, 0,             NAME,  0, STD, 155,  10,  23, 200, 32, 3,  "Heat Rejection Name:", RIGHT,   -8, 5, 0, LEFT, 4, 5, "Name of the heat rejection component; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 12900, 12900, 0, 1, HEAT-REJECTION, 0,             TYPE,  0, STD, 430,  10, 300, 130, 19, 3,                 "Type:", RIGHT,   -8, 5, 0, LEFT, 4, 5, "Open Tower=Direct evap cool;Open Tower & HX=heat exchanger transfers heat between fluids"

   LABEL,  "Loop Assignment", STD, LEFT, 20,  55, 1, 0, 0, 190, 19133, 3
   COMBO, 19133, 19133, 0, 1, HEAT-REJECTION, 0,          CW-LOOP,  0, STD,  55,  75, 200, 140, 19, 3,                   "CW:",  LEFT,  -35, 5, 0, LEFT, 4, 5, "Name of the condenser water (or heat pump) Loop that this Heat Rejection serves"
  
   LABEL, "Meter Assignment", STD, LEFT, 20, 120, 1, 0, 0, 190, 12359, 3
   COMBO, 12359, 12209, 0, 1, HEAT-REJECTION, 0,       ELEC-METER,  0, STD, 110, 140, 120,  80, 19, 3,       "Electric Meter:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electric consumption of this tower"
    
; SAC 10/24/00 - added compliance inputs
   LABEL, "Compliance Inputs",   STD, LEFT, 20, 185, 0, 0, 1, 190, 15520, 3
    EDIT, 15520,     0, 0, 1, HEAT-REJECTION, 0,   C-NUM-OF-UNITS, -1, STD, 120, 205,  23,  50,  0, 3,      "Number of Units:",  LEFT, -100, 5, 1, LEFT, 4, 5, "The total number of cooling towers or fluid coolers simulated as one"

;   LABEL, "Design Parameters", STD, LEFT, 20, 205, 1, 0, 0, 190, 12360, 3
;    EDIT, 12360, 12210, 0, 1, HEAT-REJECTION, 0,   DESIGN-WETBULB, -1, STD, 120, 225,  23,  50,  1, 3,              "Wetbulb:",  LEFT, -100, 5, 1, LEFT, 4, 5, ""
;    EDIT, 12361, 12211, 0, 1, HEAT-REJECTION, 0,  DESIGN-APPROACH, -1, STD, 120, 250,  23,  50,  1, 3,             "Approach:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Difference between temperature of fluid leaving tower, and ambient air wetbulb temperature"
;    EDIT, 12507, 12212, 0, 1, HEAT-REJECTION, 0,     DESIGN-RANGE, -1, STD, 120, 275,  23,  50,  1, 3,                "Range:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Fluid DT through heat rejection; used to calc design flowrate; applies to Open Tower & HX only"
; SAC 11/30/10 - added for DOE-2.3
   LABEL, "Rated vs. Design Conditions", STD, LEFT, 20, 273, 1, 0, 0, 250, 0, 3
   LABEL, "Design", STD, CENTER, 120, 288, 1, 0, 0, 0, 12360, 3
    EDIT, 12360, 12210, 0, 1, HEAT-REJECTION, 0,   DESIGN-WETBULB, -1, STD,  85, 305,  23,  50,  1, 3,              "Wetbulb:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "The DESIGN wetbulb temperature, default is the design-day value"
    EDIT, 12361, 12211, 0, 1, HEAT-REJECTION, 0,  DESIGN-APPROACH, -1, STD,  85, 330,  23,  50,  1, 3,             "Approach:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "The DESIGN approach, default is the design-day value"
    EDIT, 12507, 12212, 0, 1, HEAT-REJECTION, 0,     DESIGN-RANGE, -1, STD,  85, 355,  23,  50,  1, 3,                "Range:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "The DESIGN temperature drop, default is the design-day value"
    EDIT, 18012,     0, 0, 1, HEAT-REJECTION, 0, DESIGN-INLETS-TD, -1, STD,  85, 380,  23,  50,  1, 3,             "Inlet dT:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "The design drybulb temperature differential across the coil, default is design day"
   LABEL, "Rated", STD, CENTER, 185, 288, 1, 0, 0, 0, 18012, 3
    EDIT, 18013,     0, 0, 1, HEAT-REJECTION, 0,  RATED-WETBULB,   -1, STD, 150, 305,  23,  50,  1, 3,                      "",  LEFT,   -1, 5, 1, LEFT, 4, 5, "The RATED wetbulb for which capacity and power consumption is specified"
    EDIT, 18014,     0, 0, 1, HEAT-REJECTION, 0,  RATED-APPROACH,  -1, STD, 150, 330,  23,  50,  1, 3,                      "",  LEFT,   -1, 5, 1, LEFT, 4, 5, "The RATED approach for which capacity and power consumption is specified"
    EDIT, 18015,     0, 0, 1, HEAT-REJECTION, 0,  RATED-RANGE,     -1, STD, 150, 355,  23,  50,  1, 3,                      "",  LEFT,   -1, 5, 1, LEFT, 4, 5, "The RATED temperature drop for which capacity and power consumption is specified"
    EDIT, 18016,     0, 0, 1, HEAT-REJECTION, 0,  RATED-INLETS-TD, -1, STD, 150, 380,  23,  50,  1, 3,                      "",  LEFT,   -1, 5, 1, LEFT, 4, 5, "The drybulb temperature differential across the coil needed to achieve the rated heat rejection capacity"

   LABEL, "Equipment Capacity", STD, LEFT, 230, 55, 1, 0, 0, 405, 12362, 3
    EDIT, 12362, 12190, 0, 1, HEAT-REJECTION, 0,         CAPACITY, -1, STD, 305,  75,  23,  75,  1, 3,            "Total Cap:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Nominal (rated) cooling capacity in MBTU/hr (e.g., 100 ton = 1.2 MBTU/hr)"
    EDIT, 12369, 12201, 0, 1, HEAT-REJECTION, 0,   CAPACITY-RATIO, -1, STD, 330, 100,  23,  50,  2, 3,       "Capacity Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Capacity as fraction of max cooling load (used only if DOE-2 sizes the tower)"
    EDIT, 12374, 12202, 0, 1, HEAT-REJECTION, 0,  NUMBER-OF-CELLS, -1, STD, 330, 125,  23,  50,  0, 3,         "Num of Cells:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Total number of cells in the heat rejection"
    
   LABEL, "Cell Control", STD, LEFT, 230, 160, 1, 0, 0, 405, 12526, 3
   COMBO, 12526, 12131, 0, 1, HEAT-REJECTION, 0,        CELL-CTRL,  0, STD, 295, 180,  80, 110, 19, 3,            "Cell Ctrl:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "Min Cells=maximise flow through each cell;Max Cells =minimize flow through each cell"
    EDIT, 12465, 12465, 0, 1, HEAT-REJECTION, 0,    MAX-FLOW/CELL, -1, STD, 330, 205,  23,  50,  2, 3,        "Cell Max Flow:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Largest allowable ratio of actual flow rate to design flow rate (for each cell)"
    EDIT, 12466, 12466, 0, 1, HEAT-REJECTION, 0,    MIN-FLOW/CELL, -1, STD, 330, 230,  23,  50,  2, 3,        "Cell Min Flow:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Smallest allowable ratio of actual flow rate to design flow rate (for each cell)"
   
   LABEL, "Fan Efficiency", STD, LEFT, 450, 55, 1, 0, 0, 645, 0, 3
    EDIT, 12508, 12207, 0, 1, HEAT-REJECTION, 0,      FAN-KW/CELL, -1, STD, 560,  75,  23,  65,  1, 3,      "Fan kW per Cell:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Power consumption of the heat rejection fan (per cell), at the rated flow rate"
    EDIT, 12524, 12206, 0, 1, HEAT-REJECTION, 0, ELEC-INPUT-RATIO, -1, STD, 560, 100,  23,  65,  4, 3,     "Elec Input Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Dimensionless ratio of electric input power to nominal tower capacity"

   LABEL, "Fan Control", STD, LEFT, 450, 160, 1, 0, 0, 645, 12510, 3
   COMBO, 12510, 12122, 0, 1, HEAT-REJECTION, 0,    CAPACITY-CTRL,  0, STD, 510, 180, 110, 135, 19, 3,             "Cap Ctrl:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "1SpdFan=cycles on/off;Fluid Bypass=via valve;2SpdFan=cycles off/low/on;Var. Fan modulates"
    EDIT, 12468, 12468, 0, 1, HEAT-REJECTION, 0, FAN-OFF-AIR-FLOW, -1, STD, 575, 205,  23,  50,  2, 3,         "Fan Off Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Ratio of airflow through tower due to natural convection (fans off), to flow at design fan speed"
    EDIT, 12474, 12474, 0, 1, HEAT-REJECTION, 0, FAN-LOW-AIR-FLOW, -1, STD, 575, 230,  23,  50,  2, 3,         "Fan Low Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "For 2 speed fans: ratio of power consumption when fans at low speed to that at design speed"
    EDIT, 12476, 12476, 0, 1, HEAT-REJECTION, 0,       FAN-LOW-KW, -1, STD, 575, 255,  23,  50,  2, 3,         "Fan Low Elec:",  LEFT, -125, 5, 1, LEFT, 4, 5, "For 2 speed fans: ratio of power consumption when fans at low speed to that at design speed"
    EDIT, 12478, 12478, 0, 1, HEAT-REJECTION, 0,    MIN-VFD-SPEED, -1, STD, 575, 280,  23,  50,  2, 3,          "Min Fan Spd:",  LEFT, -125, 5, 1, LEFT, 4, 5, "For varaible speed fans: ratio of minimum allowable speed to nominal fan speed"
    EDIT, 14276, 14276, 0, 1, HEAT-REJECTION, 0,    MIN-RESET-PLR, -1, STD, 575, 305,  23,  50,  2, 3,        "Min Reset PLR:",  LEFT, -125, 5, 1, LEFT, 4, 5, "For varaible speed fans: ratio of minimum allowable speed to nominal fan speed"
    EDIT, 14277, 14277, 0, 1, HEAT-REJECTION, 0,  MAX-RESET-SPEED, -1, STD, 575, 330,  23,  50,  2, 3,      "Max Reset Speed:",  LEFT, -125, 5, 1, LEFT, 4, 5, "For varaible speed fans: ratio of minimum allowable speed to nominal fan speed"

  ;******************************************
  ; Heat Rejection - Fluid & Dry Coolers Page
  ;******************************************
  TABPAGE, 3005, 32068, 1, 3, NOTIMP, " Fluid and Dry Coolers "
   
   LABEL,                "Dry Cooler and", STD, LEFT, 40,  39, 1, 0, 0, 0, 0, 3
   LABEL,  "Fluid Cooler, Dry Operation",  STD, LEFT, 40,  55, 1, 0, 0, 300, 0, 3
; SAC 11/30/10 - removed for DOE-2.3
;   COMBO, 14332, 14273, 0, 1, HEAT-REJECTION, 0,           DRY-HX,  0, STD, 150,  75, 200, 150, 19, 3,              "HX Name:",  LEFT, -110, 5, 0, LEFT, 4, 5, ""
;    EDIT, 14333, 14274, 0, 1, HEAT-REJECTION, 0,     DRY-INLET-DT, -1, STD, 150, 100,  23,  65,  1, 3,    "Dry Inlet Delta T:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
    EDIT, 14334, 14334, 0, 1, HEAT-REJECTION, 0, AIR-TO-FLUID-FLO, -1, STD, 150,  75,  23,  65,  1, 3,    "Air-to-Fluid Flow:",  LEFT, -110, 5, 1, LEFT, 4, 5, "For a fluid cooler running dry, the ratio of RATED airflow to fluid flow"
; SAC 11/30/10 - added for DOE-2.3
    EDIT, 18010,     0, 0, 1, HEAT-REJECTION, 0,   AIRFLOW-TD/CAP, -1, STD, 150, 100,  23,  65,  1, 3,     "Airflow-TD / Cap:",  LEFT, -110, 5, 1, LEFT, 4, 5, "For a drycooler, the ratio of airflow to rated capacity per degree temperature differential"
    EDIT, 18011,     0, 0, 1, HEAT-REJECTION, 0,    POWER/AIRFLOW, -1, STD, 150, 125,  23,  65,  1, 3,      "Power / Airflow:",  LEFT, -110, 5, 1, LEFT, 4, 5, "The ratio of the full-load power of the drycooler fan(s) to the fan airflow at sea level"
   COMBO, 14335, 14335, 0, 1, HEAT-REJECTION, 0,     WET-COIL-SCH,  0, STD, 150, 150, 200, 150, 19, 3,         "Wet Schedule:",  LEFT, -110, 5, 0, LEFT, 4, 5, ""
    EDIT, 14336, 14336, 0, 1, HEAT-REJECTION, 0,    DRY-AIR-RATIO, -1, STD, 150, 175,  23,  65,  2, 3,        "Dry Air Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
; SAC 11/30/10 - removed for DOE-2.3
;  BUTTON, 10324, 10324, 0, 1, 92, 2506,                                STD, 150, 202,  23, 125,     3, "Heat Exchanger", "Heat Exchanger Properties"
  
   LABEL, "Fluid Cooler Spray", STD, LEFT, 40, 260, 1, 0, 0, 300, 14337, 3
    EDIT, 14337, 14270, 0, 1, HEAT-REJECTION, 0,    SPRAY-KW/CELL, -1, STD, 150, 280,  23,  65,  1, 3,            "kW / Cell:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
    EDIT, 14338, 14271, 0, 1, HEAT-REJECTION, 0,    SPRAY-KW/FLOW, -1, STD, 150, 305,  23,  65,  4, 3,            "kW / Flow:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
   COMBO, 14339, 14272, 0, 1, HEAT-REJECTION, 0,  SPRAY-PUMP-CTRL,  0, STD, 150, 330, 200, 150, 19, 3,            "Pump Ctrl:",  LEFT, -110, 5, 0, LEFT, 4, 5, ""
   
   LABEL, "Fluid Cooler Off-Hour Losses", STD, LEFT, 390, 39, 1, 0, 0, 0,   14340, 3
   LABEL,  "and Coil Freeze Protection",  STD, LEFT, 390, 55, 1, 0, 0, 620, 14340, 3
    EDIT, 14340, 14340, 0, 1, HEAT-REJECTION, 0,        COIL-LOSS,  0, STD, 535,  75,  23,  65,  0, 3,            "Coil Loss:",  LEFT, -145, 5, 1, LEFT, 4, 5, ""
    EDIT, 14341, 14341, 0, 1, HEAT-REJECTION, 0,  COIL-LOSS-RATIO,  0, STD, 535, 100,  23,  65,  2, 3,      "Coil Loss Ratio:",  LEFT, -145, 5, 1, LEFT, 4, 5, ""
    EDIT, 14342, 14342, 0, 1, HEAT-REJECTION, 0,     COIL-FLUID-T,  0, STD, 535, 125,  23,  65,  1, 3,         "Coil Fluid T:",  LEFT, -145, 5, 1, LEFT, 4, 5, ""
    EDIT, 14343, 14343, 0, 1, HEAT-REJECTION, 0,   COIL-AMBIENT-T,  0, STD, 535, 150,  23,  65,  1, 3,       "Coil Ambient T:",  LEFT, -145, 5, 1, LEFT, 4, 5, ""
    EDIT, 14344, 14344, 0, 1, HEAT-REJECTION, 0,   COIL-WINDSPEED,  0, STD, 535, 175,  23,  65,  1, 3,       "Coil Windspeed:",  LEFT, -145, 5, 1, LEFT, 4, 5, ""

  ;******************************************
  ; Heat Rejection - Performance Curves Page
  ;******************************************
  TABPAGE, 3035, 32068, 1, 3, NOTIMP, " Performance Curves "

   LABEL,  "Fan Power", STD, CENTER, 230, 25, 1, 0, 0, 0, 0, 3
   COMBO, 14278, 14278, 0, 1, HEAT-REJECTION, 0,   FAN-KW-FSPEED,  0, STD, 150,  45, 200, 165, 19, 3,   "f(fan motor speed):",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
   COMBO, 12529, 12529, 0, 1, HEAT-REJECTION,  0, FAN-KW-FDAMPER,  0, STD, 150,  80, 200, 165, 19, 3,        "f(fan damper):",  LEFT, -130, 5, 0, LEFT, 4, 5, ""
    
   LABEL, "Capacity", STD, CENTER, 415, 25, 1, 0, 0, 0, 0, 3
   COMBO, 12530, 12530, 0, 1, HEAT-REJECTION,  0,    CAP-FAPP&WB,  0, STD, 335, 115, 200, 165, 19, 3, "f(approach, wetbulb):",  LEFT, -315, 5, 0, LEFT, 4, 5, "Bi-Quadratic Equation used to determine Capacity - use of the default is highly recommended"
   COMBO, 14279, 14279, 0, 1, HEAT-REJECTION,  0,    CAP-FRNG&WB,  0, STD, 335, 145, 200, 165, 19, 3,   "f(range*, wetbulb):",  LEFT, -315, 5, 0, LEFT, 4, 5, "Bi-Quadratic Equation used to determine Capacity - use of the default is highly recommended"
   COMBO, 14533, 14533, 0, 1, HEAT-REJECTION,  0,   CAP-FAIRFLOW,  0, STD, 335, 175, 200, 165, 19, 3,       "f(twr airflow):",  LEFT, -315, 5, 0, LEFT, 4, 5, ""

    EDIT, 14281, 14281, 0, 1, HEAT-REJECTION,  0,      MAX-RANGE, -1, STD, 600, 145,  23,  50,  1, 3,           "Max Range*:",  LEFT,  -85, 5, 1, LEFT, 4, 5, ""

   LABEL, "*Maximum Range restricts the value of Range to be used in the capacity = f(tower range, tower wetbulb) curve.", STD, LEFT, 20, 205, 1, 0, 0, 0, 0, 3
   
  ;******************************************
  ; Heat Rejection - Attachments Page
  ;******************************************
  TABPAGE, 3036, 32068, 1, 3, NOTIMP, " Attachments "

   LABEL, "Recirculation Loop", STD, LEFT, 40, 30, 1, 0, 0, 265, 12532, 3
; SAC 11/30/10 - added for DOE-2.3
   COMBO, 18009,     0, 0, 1, HEAT-REJECTION, 0, CW-SERIES-LOCN,  0, STD, 155,  50, 200, 110, 19, 3, "Series Location:",  LEFT, -100, 5, 0, LEFT, 4, 5, "For a cooling tower in series, whether at the upstream or downstream location"
   COMBO, 12532, 12532, 0, 1, HEAT-REJECTION, 0,        CW-PUMP,  0, STD, 115,  75, 200, 150, 19, 3,            "Pump:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Name of Pump that serves the tower fluid; required if tower Type is Open Tower & HX"
   COMBO, 12551, 12551, 0, 1, HEAT-REJECTION, 0,   CW-FLOW-CTRL,  0, STD, 115, 100,  80, 150, 19, 3,       "Flow Ctrl:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Applies only if there is a condenser water pump; otherwise defaults to Loop Flow Control"
; SAC 1/16/06 - Design sizing mods
;   EDIT, 12563, 12563, 0, 1, HEAT-REJECTION, 0,          CW-DT, -1, STD, 165, 100,  23,  50,  1, 3,         "Delta T:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Design temperature drop of the fluid through the tower"
    EDIT, 12564, 12564, 0, 1, HEAT-REJECTION, 0,        CW-HEAD, -1, STD, 165, 125,  23,  50,  1, 3,            "Head:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Design delta P through tower due to friction (not including any Static Head); for HX towers only"
    EDIT, 12565, 12565, 0, 1, HEAT-REJECTION, 0, CW-STATIC-HEAD, -1, STD, 165, 150,  23,  50,  1, 3,     "Static Head:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Tower static head: equal to distance between spray nozzles and water level in the sump"
    EDIT, 12585, 12585, 0, 1, HEAT-REJECTION, 0,    CW-MIN-FLOW, -1, STD, 165, 175,  23,  50,  1, 3,    "Minimum Flow:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Minimum fluid flow rate through the tower; below this, tower pump cycles on & off"
;SDG 3/21/13 Hybrid GLHP 
    EDIT, 18104, 18104, 0, 1, HEAT-REJECTION, 0, CW-BYPASS-FLOW, -1, STD, 165, 200,  23,  50,  1, 3,     "Bypass Flow:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Fraction of the total loop flow that will be conditioned by the tower, but that is bypassed around the tower"
;  COMBO, 12590, 12590, 0, 1, HEAT-REJECTION, 0,   CW-ISOLATION,  0, STD, 165, 200,  80,  55, 19, 3,       "Isolation:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Whether an isolation valve exists to shunt the fluid flow; if no tower Pump, fluid always flows"

   LABEL, "Heat Exchanger", STD, LEFT, 395, 30, 1, 0, 0, 540, 14284, 3
; SAC 1/16/06 - Design sizing mods
;   COMBO, 14282, 14269, 0, 1, HEAT-REJECTION, 0,          CW-HX,  0, STD, 410,  50,  80, 150, 19, 3,       "HX Name:",  LEFT,  -70, 5, 0, LEFT, 4, 5, ""
;    EDIT, 14283, 12208, 0, 1, HEAT-REJECTION, 0,          HX-DT, -1, STD, 460,  75,  23,  50,  1, 3,       "Delta T:",  LEFT, -120, 5, 1, LEFT, 4, 5, ""
    EDIT, 14284, 14268, 0, 1, HEAT-REJECTION, 0,        HX-HEAD, -1, STD, 465,  50,  23,  50,  1, 3,          "Head:",  LEFT,  -55, 5, 1, LEFT, 4, 5, "The head on each side of the open-tower heat exchanger"
; SAC 1/16/06 - Design sizing mods
;  BUTTON, 10321, 10321, 0, 1, 92, 2506,                              STD, 410, 127,  23, 125,     3, "Heat Exchanger", "Heat Exchanger Properties"
    
  ;******************************************
  ; Heat Rejection - Miscellaneous Page
  ;******************************************
  TABPAGE, 3119, 32068, 1, 3, NOTIMP, " Miscellaneous "

   LABEL, "Pan Freeze Protection", STD, LEFT, 40, 30, 1, 0, 0, 250, 14303, 3
   COMBO, 14303, 14303, 0, 1, HEAT-REJECTION, 0,   PAN-HEATER-TYPE,  0, STD, 150,  50,  80, 100, 19, 3,  "Pan Heater Type:",  LEFT, -110, 5, 0, LEFT, 4, 5, ""
    EDIT, 14304, 14304, 0, 1, HEAT-REJECTION, 0,          PAN-LOSS,  0, STD, 150,  75,  23,  50,  0, 3,         "Pan Loss:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
    EDIT, 14305, 14305, 0, 1, HEAT-REJECTION, 0,    PAN-LOSS-RATIO,  0, STD, 150, 100,  23,  50,  3, 3,   "Pan Loss Ratio:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
    EDIT, 14306, 14306, 0, 1, HEAT-REJECTION, 0,       PAN-FLUID-T,  0, STD, 150, 125,  23,  50,  1, 3,      "Pan Fluid T:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
    EDIT, 14307, 14307, 0, 1, HEAT-REJECTION, 0,     PAN-AMBIENT-T,  0, STD, 150, 150,  23,  50,  1, 3,    "Pan Ambient T:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
    EDIT, 14308, 14308, 0, 1, HEAT-REJECTION, 0,     PAN-WINDSPEED,  0, STD, 150, 175,  23,  50,  1, 3,    "Pan Windspeed:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
              
   LABEL, "Freeze Protection Loop", STD, LEFT, 330, 30, 1, 0, 0, 600, 14309, 3
   COMBO, 14309, 14309, 0, 1, HEAT-REJECTION, 0,   PAN-HEATER-LOOP,  0, STD, 450,  50,  80, 150, 19, 3,  "Pan Heater Loop:",  LEFT, -120, 5, 0, LEFT, 4, 5, ""
   COMBO, 14310, 14310, 0, 1, HEAT-REJECTION, 0,    PAN-VALVE-TYPE,  0, STD, 450,  75,  80, 150, 19, 3,       "Valve Type:",  LEFT, -120, 5, 0, LEFT, 4, 5, ""
    EDIT, 14311, 14311, 0, 1, HEAT-REJECTION, 0,   PAN-HEATER-HEAD,  0, STD, 450, 100,  23,  50,  1, 3,             "Head:",  LEFT, -120, 5, 1, LEFT, 4, 5, ""
    EDIT, 14312, 14312, 0, 1, HEAT-REJECTION, 0,     PAN-HEATER-DT,  0, STD, 450, 125,  23,  50,  1, 3,   "Heater Delta T:",  LEFT, -120, 5, 1, LEFT, 4, 5, ""
              
   LABEL, "Auxiliaries", STD, LEFT, 330, 180, 1, 0, 0, 600, 12706, 3
    EDIT, 12706, 12706, 0, 1, HEAT-REJECTION, 0,            AUX-KW, -1, STD, 450, 200,  23,  50,  1, 3,            "Power:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Auxiliary electric power consumption of the heat rejection (e.g., control panels)"
   COMBO, 12901, 12901, 0, 1, HEAT-REJECTION, 0,          AUX-MODE,  0, STD, 450, 225, 110, 150, 19, 3,             "Mode:",  LEFT, -120, 5, 0, LEFT, 4, 5, "Always=all hours;When On=If tower on;When Off=if tower off;Scheduled=use Aux Schedule"
   COMBO, 12902, 12902, 0, 1, HEAT-REJECTION, 0,      AUX-SCHEDULE,  0, STD, 450, 250, 200, 150, 19, 3,         "Schedule:",  LEFT, -120, 5, 0, LEFT, 4, 5, "Schedule for Auxiliary Power consumption (set Auxiliary Mode to Scheduled to activate this)"
   COMBO, 12804, 12804, 0, 1, HEAT-REJECTION, 0,         AUX-METER,  0, STD, 450, 275, 120, 150, 19, 3,            "Meter:",  LEFT, -120, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption of this tower's auxiliaries"



;PV
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Photovoltaics Module Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

 MODTABDLG, 3352,    0, 1, 30, 30, 470, 710, 0, PV-MODULE, "Photovoltaic Module Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 17660,     0, 0, 1, PV-MODULE, 0, NAME,  0, STD, 195,  15, 400, 225, 19, 3, "Currently Active PV Module:",  LEFT, -170, 5, 0, LEFT, 4, 5, "List of all photovoltaic modules defined in project; also allows library retrieval and creation"

    ;******************************************
    ; Photovoltaics Module - Basic Specs Page
    ;******************************************
    TABPAGE, 3353,    0, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 17661,     0,     0, 1,  PV-MODULE, 0,            NAME, -1, STD, 120,  10,  23, 175, 32, 3,     "Module Name:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Name of photovoltaic module"

      COMBO, 17662,     0,     0, 1,  PV-MODULE, 0,            TYPE, -1, STD, 120,  50, 300, 175, 19, 3,     "Module Type:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Photovoltaic module type"
      COMBO, 17663,     0,     0, 1,  PV-MODULE, 0,   SIM-ALGORITHM, -1, STD, 120,  75, 220, 175, 19, 3,      "Simulation:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Algorithm used to simulate the module's performance"
      COMBO, 17664,     0,     0, 1,  PV-MODULE, 0,    GLAZING-TYPE, -1, STD, 120, 100, 220, 175, 19, 3,    "Glazing Type:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Type of glazing"
      LABEL,  "Dimensions:",  STD, LEFT, 30, 130, 1, 0, 0, 0, 0, 3
       EDIT, 17665,     0,     0, 1,  PV-MODULE, 0,          HEIGHT,  0, STD, 166, 125,  23,  70,  2, 3,          "Height:",  LEFT,  -45, 5, 1, LEFT, 4, 5, "Height of the photovoltaic module"
       EDIT, 17666,     0,     0, 1,  PV-MODULE, 0,           WIDTH,  0, STD, 166, 150,  23,  70,  2, 3,           "Width:",  LEFT,  -45, 5, 1, LEFT, 4, 5, "Width of the photovoltaic module"

; SAC 10/25/03 - Removed this entire section since these controls are no longer used
;      LABEL,  "Reference Conditions",  STD, LEFT, 30, 195, 1, 0, 0, 295, 17667, 3
;       EDIT, 17667,     0,     0, 1,  PV-MODULE, 0,    NOCT-AMBIENT,  0, STD, 185, 215,  23,  65,  2, 3,  "Ambient Temperature*:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The ambient temperature at which the nominal cell operating temperature (NOCT) is specified"
;       EDIT, 17669,     0,     0, 1,  PV-MODULE, 0,  NOCT-WINDSPEED,  0, STD, 185, 240,  23,  65,  2, 3,           "Wind Speed*:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The wind speed at which the nominal cell operating temperature (NOCT) is specified"
;       EDIT, 17668,     0,     0, 1,  PV-MODULE, 0, NOCT-IRRADIANCE,  0, STD, 185, 265,  23,  65,  1, 3,   "Ambient Irradiance*:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The ambient irradiance level at which the nominal cell operating temperature (NOCT) is specified"
;       EDIT, 17670,     0,     0, 1,  PV-MODULE, 0,  REF-IRRADIANCE,  0, STD, 185, 290,  23,  65,  1, 3,  "Reference Irradiance:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The irradiance level at which the rated cell voltages and amperages are measured (usually greater than the NOCT irradiance)"
;      LABEL,  "* specified at nominal cell operating temperature",  SMALL, LEFT, 45, 317, 1, 0, 0, 0, 17667, 3

      LABEL,  "Performance Data",  STD, LEFT, 360, 30, 1, 0, 0, 675, 0, 3
; SAC 10/25/03 - Removed first control because no longer used (???), changed labels on all other controls and added new control @ bottom
;       EDIT, 17674,     0,     0, 1,  PV-MODULE, 0,  NOM-OPER-CELL-T,  0, STD, 550,  50,  23,  90,  1, 3, "Normal Operating Cell Temp.:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The normal operating cell temperature (NOCT), when operating at the reference conditions."
;       EDIT, 17675,     0,     0, 1,  PV-MODULE, 0,   VOLTS-OPEN-CKT,  0, STD, 550,  75,  23,  90,  2, 3,   "Open Circuit (OC) Voltage:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The open circuit voltage at the reference irradiance level"
;       EDIT, 17676,     0,     0, 1,  PV-MODULE, 0,    VOLTS-MAX-PWR,  0, STD, 550, 100,  23,  90,  2, 3,     "Voltage @ Maximum Power:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The voltage at the maximum power point (always less than the open circuit voltage)"
;       EDIT, 17677,     0,     0, 1,  PV-MODULE, 0, VOLTS/T-OPEN-CKT,  0, STD, 550, 125,  23,  90,  4, 3,      "OC Voltage Change Rate:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The rate at which the open circuit voltage changes with cell temperature"
;       EDIT, 17678,     0,     0, 1,  PV-MODULE, 0,   AMPS-SHORT-CKT,  0, STD, 550, 150,  23,  90,  2, 3,  "Short Circuit (SC) Current:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The short circuit current at the reference irradiance level"
;       EDIT, 17679,     0,     0, 1,  PV-MODULE, 0,     AMPS-MAX-PWR,  0, STD, 550, 175,  23,  90,  2, 3,     "Current @ Maximum Power:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The current at the maximum power point (always less than the short circuit current)"
;       EDIT, 17680,     0,     0, 1,  PV-MODULE, 0, AMPS/T-SHORT-CKT,  0, STD, 550, 200,  23,  90,  5, 3,      "SC Current Change Rate:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The rate at which the short circuit current changes with cell temperature"
       EDIT, 17674,     0,     0, 1,  PV-MODULE, 0,   VOLTS-OPEN-CKT,  0, STD, 555,  50,  23,  75,  2, 3,   "Open Circuit Voltage, Voc:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Open circuit voltage at 1000 W/m2, 25°C and 1.5 air mass"
       EDIT, 17675,     0,     0, 1,  PV-MODULE, 0, VOLTS/T-OPEN-CKT,  0, STD, 555,  75,  23,  75,  4, 3,  "Voc Temperature Coef, BVoc:",  LEFT, -180, 5, 1, LEFT, 4, 5, "The rate at which Voc changes with temperature"
       EDIT, 17676,     0,     0, 1,  PV-MODULE, 0,   AMPS-SHORT-CKT,  0, STD, 555, 100,  23,  75,  2, 3,  "Short Circuit Current, Isc:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Short circuit current at 1000 W/m2, 25°C and 1.5 air mass"
       EDIT, 17677,     0,     0, 1,  PV-MODULE, 0, AMPS/T-SHORT-CKT,  0, STD, 555, 125,  23,  75,  5, 3,  "Isc Temperature Coef, aIsc:",  LEFT, -180, 5, 1, LEFT, 4, 5, "The rate at which Isc changes with temperature"
       EDIT, 17678,     0,     0, 1,  PV-MODULE, 0,    VOLTS-MAX-PWR,  0, STD, 555, 150,  23,  75,  2, 3,      "Max Power Voltage, Vmp:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Maximum power voltage at 1000 W/m2, 25°C and 1.5 air mass"
       EDIT, 17679,     0,     0, 1,  PV-MODULE, 0,     AMPS-MAX-PWR,  0, STD, 555, 175,  23,  75,  2, 3,      "Max Power Current, Imp:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Maximum power current at 1000 W/m2, 25°C and 1.5 air mass"
       EDIT, 17680,     0,     0, 1,  PV-MODULE, 0,     CELL-BACK-DT,  0, STD, 555, 200,  23,  75,  1, 3,      "Cell - Back Surface dT:",  LEFT, -180, 5, 1, LEFT, 4, 5, "Differential between cell temperature and back surface temperature"

      LABEL,  "Irradiance Performance Curves",  STD, LEFT, 360, 245, 1, 0, 0, 675, 0, 3
      COMBO, 17681,     0,     0, 1,  PV-MODULE, 0,   IRRADIANCE-FAM, -1, STD, 510, 265, 220, 165, 19, 3,       "f(effective air mass):",  LEFT, -135, 5, 0, LEFT, 4, 5, "Modifies the spectral properties of the plane-of-array irradiation as a function of the effective air mass between the module and the sun"
      COMBO, 17682,     0,     0, 1,  PV-MODULE, 0,  IRRADIANCE-FAOI, -1, STD, 510, 290, 220, 165, 19, 3,    "f(sun's angle of incid.):",  LEFT, -135, 5, 0, LEFT, 4, 5, "Modifies the plane-of-array irradiation transmittance as a function of the sun's angle of incidence"

      STATIC, 1, PV-MODULE, 0,    CAPACITY, -1, 0, 5,  30, 360, -1, STD, LEFT, "Calculated Information:    Capacity:  ", "", 1, 3
      STATIC, 1, PV-MODULE, 0,  EFFICIENCY, -1, 0, 3, 350, 360, -1, STD, LEFT,                          "Efficiency:  ", "", 0, 3
      STATIC, 1, PV-MODULE, 0,        AREA, -1, 0, 2, 485, 360, -1, STD, LEFT,                                "Area:  ", "", 1, 3


    ;******************************************
    ; Photovoltaics Module - Sandia/King Data Page
    ;******************************************
    TABPAGE, 3354,    0, 1, 3, NOTIMP, " Sandia/King Algorithm "

      LABEL,  "Sandia/King Algorithm Data",  STD, LEFT, 30, 30, 1, 0, 0, 350, 17685, 3
; SAC 10/25/03 - Updated labels & tooltips on existing keywords and added one new keyword
       EDIT, 17685,     0,     0, 1,  PV-MODULE, 0,  VOLTS/T-MAX-PWR,  0, STD, 235,  50,  23,  70,  4, 3,     "Vmp Temperature Coef, BVmp:",  LEFT, -190, 5, 1, LEFT, 4, 5, "The rate at which Vmp changes with temperature"
       EDIT, 17686,     0,     0, 1,  PV-MODULE, 0,  VOLTS/E-MAX-PWR,  0, STD, 235,  75,  23,  70,  4, 3,     "Vmp Irradiance Coef, mBVmp:",  LEFT, -190, 5, 1, LEFT, 4, 5, "The rate at which Vmp changes with irradiance"
       EDIT, 17687,     0,     0, 1,  PV-MODULE, 0,   AMPS/T-MAX-PWR,  0, STD, 235, 100,  23,  70,  4, 3,     "Imp Temperature Coef, aImp:",  LEFT, -190, 5, 1, LEFT, 4, 5, "The rate at which Imp changes with temperature"
       EDIT, 17688,     0,     0, 1,  PV-MODULE, 0,     CELLS-SERIES,  0, STD, 235, 125,  23,  70,  0, 3,      "Number of Cells in Series:",  LEFT, -190, 5, 1, LEFT, 4, 5, "Number of cells in series within the module"

      LABEL,  "King Equation Coefficients",  STD, LEFT, 420, 30, 1, 0, 0, 640, 17689, 3
; SAC 10/25/03 - Updated decimal precisions
       EDIT, 17689,     0,     0, 1,  PV-MODULE, 0,               C0,  0, STD, 515,  50,  23,  80,  6, 3,            "C0:", LEFT,  -80, 5, 1, LEFT, 4, 5, "C0 coefficient in the King equations"
       EDIT, 17690,     0,     0, 1,  PV-MODULE, 0,               C1,  0, STD, 515,  75,  23,  80,  6, 3,            "C1:", LEFT,  -80, 5, 1, LEFT, 4, 5, "C1 coefficient in the King equations"
       EDIT, 17691,     0,     0, 1,  PV-MODULE, 0,               C2,  0, STD, 515, 100,  23,  80,  6, 3,            "C2:", LEFT,  -80, 5, 1, LEFT, 4, 5, "C2 coefficient in the King equations"
       EDIT, 17692,     0,     0, 1,  PV-MODULE, 0,               C3,  0, STD, 515, 125,  23,  80,  6, 3,            "C3:", LEFT,  -80, 5, 1, LEFT, 4, 5, "C3 coefficient in the King equations"
       EDIT, 17693,     0,     0, 1,  PV-MODULE, 0,           FDIODE,  0, STD, 515, 150,  23,  80,  4, 3,  "Diode-Effect:", LEFT,  -80, 5, 1, LEFT, 4, 5, "Diode-effect coefficient in the King equations"

; SAC 10/25/03 - New section w/ newly added keywords
      LABEL,  "Air Mass and Incident Angle Polynomials",  STD, LEFT, 30, 220, 1, 0, 0, 655, 17667, 3
       EDIT, 17667,     0,     0, 1,  PV-MODULE, 0,            A0-A4,  0, STD, 135, 240,  23, 100, 10, 3,        "Air Mass:",  LEFT, -90, 5, 0, LEFT, 4, 5, "4th-order polynomial modifying irradiance as a function of air mass"
       EDIT, 17669,     0,     0, 1,  PV-MODULE, 0,            A0-A4,  1, STD, 240, 240,  23, 100, 10, 3,                 "",  LEFT,   0, 0, 0, LEFT, 4, 5, "4th-order polynomial modifying irradiance as a function of air mass"
       EDIT, 17668,     0,     0, 1,  PV-MODULE, 0,            A0-A4,  2, STD, 345, 240,  23, 100, 10, 3,                 "",  LEFT,   0, 0, 0, LEFT, 4, 5, "4th-order polynomial modifying irradiance as a function of air mass"
       EDIT, 17670,     0,     0, 1,  PV-MODULE, 0,            A0-A4,  3, STD, 450, 240,  23, 100, 10, 3,                 "",  LEFT,   0, 0, 0, LEFT, 4, 5, "4th-order polynomial modifying irradiance as a function of air mass"
       EDIT, 17830,     0,     0, 1,  PV-MODULE, 0,            A0-A4,  4, STD, 555, 240,  23, 100, 10, 3,                 "",  LEFT,   0, 0, 0, LEFT, 4, 5, "4th-order polynomial modifying irradiance as a function of air mass"
       EDIT, 17831,     0,     0, 1,  PV-MODULE, 0,            B0-B5,  0, STD, 135, 270,  23, 100, 10, 3,  "Incident Angle:",  LEFT, -90, 5, 0, LEFT, 4, 5, "5th-order polynomial modifying irradiance transmission for incident angle"
       EDIT, 17832,     0,     0, 1,  PV-MODULE, 0,            B0-B5,  1, STD, 240, 270,  23, 100, 10, 3,                 "",  LEFT,   0, 0, 0, LEFT, 4, 5, "5th-order polynomial modifying irradiance transmission for incident angle"
       EDIT, 17833,     0,     0, 1,  PV-MODULE, 0,            B0-B5,  2, STD, 345, 270,  23, 100, 10, 3,                 "",  LEFT,   0, 0, 0, LEFT, 4, 5, "5th-order polynomial modifying irradiance transmission for incident angle"
       EDIT, 17834,     0,     0, 1,  PV-MODULE, 0,            B0-B5,  3, STD, 450, 270,  23, 100, 10, 3,                 "",  LEFT,   0, 0, 0, LEFT, 4, 5, "5th-order polynomial modifying irradiance transmission for incident angle"
       EDIT, 17835,     0,     0, 1,  PV-MODULE, 0,            B0-B5,  4, STD, 555, 270,  23, 100, 10, 3,                 "",  LEFT,   0, 0, 0, LEFT, 4, 5, "5th-order polynomial modifying irradiance transmission for incident angle"
       EDIT, 17836,     0,     0, 1,  PV-MODULE, 0,            B0-B5,  5, STD, 240, 295,  23, 100, 10, 3,                 "",  LEFT,   0, 0, 0, LEFT, 4, 5, "5th-order polynomial modifying irradiance transmission for incident angle"
      LABEL,  "* Note: If specified, these polynomials will override the Irradiance Performance Curves specified under Basic Specifications",  SMALL, LEFT, 45, 322, 1, 0, 0, 0, 17667, 3


; No PV-MODULE UI for now
;  27> COST-DATA                           Symbolic Undef      1   91 (MATERIALS-COST  )  TABLE =0   27         -7 (*No Default*    )
;  28> EQUIPMENT-REPORT                    Symbolic Defined    1  112 (CODE-WORD       )  TABLE =0   28         33 (YES             )
;  29> PICTURE                               Numeric Rounded    1            1.00       100000.00  29  -77777.00 *No Default*    
;  30> DRAWING                               Numeric Rounded    1            1.00       100000.00  30  -77777.00 *No Default*    



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Electric Generator Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

 MODTABDLG, 3164, 32070, 1, 100, 100, 470, 710, 0, ELEC-GENERATOR, "Electric Generator Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 12516, 12516, 0, 1, ELEC-GENERATOR, 0, NAME,  0, STD, 240,  15, 400, 250, 19, 3, "Currently Active Electric Generator:", RIGHT,   -8, 5, 0, LEFT, 4, 5, "List of all electric generator components defined in project; also allows library retrieval and creation"
   STATIC, 1, ELEC-GENERATOR, 0, TYPE, 0, 0, 0, 510, 20, 300, STD, LEFT, "Type: ",   "", 0, 3

  ;******************************************
  ;  Electric Generator - Basic Specifications Page
  ;******************************************
  TABPAGE, 3165, 32070, 1, 3, NOTIMP, " Basic Specifications "
    
    EDIT, 12533, 12533, 0, 1, ELEC-GENERATOR, 0,             NAME,  0, STD, 175,  10,  23, 250, 32, 3,  "Electric Generator Name:", RIGHT,   -8, 5, 0, LEFT, 4, 5, "Name of the electric generator component; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 12569, 12569, 0, 1, ELEC-GENERATOR, 0,             TYPE,  0, STD, 175,  35, 300, 250, 19, 3,                     "Type:", RIGHT,   -8, 5, 0, LEFT, 4, 5, ""

   LABEL, "Meter Assignments", STD, LEFT, 20, 80, 1, 0, 0, 220, 15385, 3
   COMBO, 15384, 15384, 0, 1, ELEC-GENERATOR, 0,       FUEL-METER,  0, STD, 115, 100, 200, 105, 19, 3,            "Fuel Meter:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "Name of the Fuel Meter that tallies the fuel consumption of this generator"
   COMBO, 15385, 15385, 0, 1, ELEC-GENERATOR, 0,       ELEC-METER,  0, STD, 115, 125, 200, 105, 19, 3,        "Electric Meter:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption"
   COMBO, 15386, 15386, 0, 1, ELEC-GENERATOR, 0,    SURPLUS-METER,  0, STD, 115, 150, 200, 105, 19, 3,         "Surplus Meter:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the surplus power generation to be sold"

   CASE, ELEC-GENERATOR, 0, TYPE, -1, =, 1, 4   ; PV ARRAY version
      LABEL, "Equipment Capacity", STD, LEFT, 260, 80, 1, 0, 0, 430, 15388, 3
       EDIT, 15388, 15388, 0, 1, ELEC-GENERATOR, 0,         CAPACITY,  0, STD, 330, 100,  23,  75,  3, 3,              "Capacity:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "Nominal (rated) capacity per inverter"
       EDIT, 17748, 17708, 0, 1, ELEC-GENERATOR, 0,    NUM-INVERTERS,  0, STD, 355, 125,  23,  50,  0, 3,        "# of Inverters:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "the number of inverters that operate in parallel"
       EDIT, 15389, 15389, 0, 1, ELEC-GENERATOR, 0,        MIN-RATIO,  0, STD, 355, 150,  23,  50,  2, 3,         "Minimum Ratio:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Minimum generator operating ratio (a fraction of the Capacity)"
       EDIT, 15390, 15390, 0, 1, ELEC-GENERATOR, 0,        MAX-RATIO,  0, STD, 355, 175,  23,  50,  2, 3,         "Maximum Ratio:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Maximum allowable generator operating ratio (a fraction of the Capacity)"

      LABEL, "Availability", STD, LEFT, 260, 230, 1, 0, 0, 430, 15387, 3
       EDIT, 15387, 15387, 0, 1, ELEC-GENERATOR, 0,    START-UP-TIME,  0, STD, 355, 250,  23,  50,  2, 3,         "Start-up Time:",  LEFT,  -95, 5, 1, LEFT, 4, 5, ""

      LABEL, "Equipment Efficiency", STD, LEFT, 470, 80, 1, 0, 0, 685, 0, 3
       EDIT, 15391, 15391, 0, 1, ELEC-GENERATOR, 0,         MECH-EFF,  0, STD, 600, 100,  23,  60,  2, 3, "Mechanical Efficiency:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""
       EDIT, 15392, 15392, 0, 1, ELEC-GENERATOR, 0, HEAT-INPUT-RATIO,  0, STD, 600, 125,  23,  60,  2, 3,      "Heat Input Ratio:",  LEFT, -130, 5, 1, LEFT, 4, 5, "the ratio of design fuel consumption to design electrical output, when both are in the same units"
; SAC 3/30/03 - Implemented ELEC-INPUT-RATIO edit control for PV array stuff
       EDIT, 15393, 17709, 0, 1, ELEC-GENERATOR, 0, ELEC-INPUT-RATIO,  0, STD, 600, 150,  23,  60,  4, 3,      "Elec Input Ratio:",  LEFT, -130, 5, 1, LEFT, 4, 5, "the ratio of direct-current input power to alternating-current output power (at rated conditions)"
   ENDCASE
   CASE, ELSE   ; NON-PV ARRAY version
      LABEL, "Equipment Capacity", STD, LEFT, 260, 80, 1, 0, 0, 430, 17740, 3
       EDIT, 17740, 15388, 0, 1, ELEC-GENERATOR, 0,         CAPACITY,  0, STD, 335, 100,  23,  70,  1, 3,              "Capacity:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Capacity of the generator (in kW)"
       EDIT, 17741, 15389, 0, 1, ELEC-GENERATOR, 0,        MIN-RATIO,  0, STD, 355, 125,  23,  50,  2, 3,         "Minimum Ratio:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Minimum generator operating ratio (a fraction of the Capacity)"
       EDIT, 17742, 15390, 0, 1, ELEC-GENERATOR, 0,        MAX-RATIO,  0, STD, 355, 150,  23,  50,  2, 3,         "Maximum Ratio:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Maximum allowable generator operating ratio (a fraction of the Capacity)"

      LABEL, "Availability", STD, LEFT, 260, 230, 1, 0, 0, 430, 17744, 3
       EDIT, 17744, 15387, 0, 1, ELEC-GENERATOR, 0,    START-UP-TIME,  0, STD, 355, 250,  23,  50,  2, 3,         "Start-up Time:",  LEFT,  -95, 5, 1, LEFT, 4, 5, ""

      LABEL, "Equipment Efficiency", STD, LEFT, 470, 80, 1, 0, 0, 685, 0, 3
       EDIT, 17746, 15391, 0, 1, ELEC-GENERATOR, 0,         MECH-EFF,  0, STD, 600, 100,  23,  60,  2, 3, "Mechanical Efficiency:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""
       EDIT, 17747, 15392, 0, 1, ELEC-GENERATOR, 0, HEAT-INPUT-RATIO,  0, STD, 600, 125,  23,  60,  2, 3,      "Heat Input Ratio:",  LEFT, -130, 5, 1, LEFT, 4, 5, "the ratio of design fuel consumption to design electrical output, when both are in the same units"
   ENDCASE


  ;******************************************
  ;  Electric Generator - Performance Curves Page
  ;******************************************
  TABPAGE, 3220, 32070, 1, 3, NOTIMP, " Performance Curves "

   LABEL,  "f(part load ratio):",  STD, LEFT, 20,  50, 1, 0, 0, 0,     0, 3
   LABEL,  "f(t water entering,",  STD, LEFT, 20,  74, 1, 0, 0, 0,     0, 3
   LABEL,  "t water leaving):",    STD, LEFT, 30,  87, 1, 0, 0, 0,     0, 3
   LABEL,  "f(part load ratio):",  STD, LEFT, 20, 155, 1, 0, 0, 0,     0, 3

   LABEL,  "f(stm pres entering,", STD, LEFT, 20, 214, 1, 0, 0, 0,     0, 3
   LABEL,  "stm pres leaving):",   STD, LEFT, 30, 227, 1, 0, 0, 0,     0, 3

   LABEL,  "Heat Input Ratio", STD, CENTER, 230, 25, 1, 0, 0, 0, 0, 3
   COMBO, 15394, 15394, 0, 1, ELEC-GENERATOR, 0,        HIR-FPLR,  0, STD, 150,  45, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Heat Input Ratio as a function of the part load ratio"
   COMBO, 15395, 15395, 0, 1, ELEC-GENERATOR, 0,          HIR-FT,  0, STD, 150,  80, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Bi-Quadratic Curve: the HIR as a function of the temp of entering and exiting water"

   LABEL,  "Exhaust Heat Recovery", STD, CENTER, 230, 130, 1, 0, 0, 0, 15396, 3
   COMBO, 15396, 15396, 0, 1, ELEC-GENERATOR, 0,   EXH-RCVR-FPLR,  0, STD, 150, 150, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Exhaust Heat Recovery as a function of the part load ratio"

; SAC 3/30/03 - Implemented EIR-FPLR combo for PV array stuff
   LABEL, "Electric Input Ratio", STD, CENTER, 415, 25, 1, 0, 0, 0, 15397, 3
   COMBO, 15397, 15397, 0, 1, ELEC-GENERATOR, 0,        EIR-FPLR,  0, STD, 335,  45, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Linear or Quadratic Curve Fit: Electric Input Ratio as a function of the part load ratio"

   LABEL,  "Jacket Heat Recovery", STD, CENTER, 415, 130, 1, 0, 0, 0, 15398, 3
   COMBO, 15398, 15398, 0, 1, ELEC-GENERATOR, 0,   JAC-RCVR-FPLR,  0, STD, 335, 150, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: Jacket Heat Recovery as a function of the part load ratio"


   LABEL, "Capacity", STD, CENTER, 600, 25, 1, 0, 0, 0, 15399, 3
   COMBO, 15399, 15399, 0, 1, ELEC-GENERATOR, 0,     CAPACITY-FT,  0, STD, 520,  80, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Bi-Quadratic Curve: Capacity as a function of the temp of entering and exiting water"

   LABEL,  "Steam Consumption Rate", STD, CENTER, 600, 200, 1, 0, 0, 0, 15400, 3
   COMBO, 15400, 15400, 0, 1, ELEC-GENERATOR, 0, STEAM-ENTH-FP&P,  0, STD, 520, 220, 200, 165, 19, 3, "",  LEFT, 0, 5, 0, LEFT, 4, 5, "Bi-Quadratic Curve: Steam Consumption Rate as a function of entering and exiting steam pressure"


  ;******************************************
  ;  Electric Generator - Loop Attachments Page
  ;******************************************
  TABPAGE, 3219, 32070, 1, 3, NOTIMP, " Loop Attachments "

   LABEL, "Heat Recovery", STD, LEFT, 20,  30, 1, 0, 0, 340, 15401, 3
   COMBO, 15401, 15401, 0, 1, ELEC-GENERATOR, 0,          EXH-LOOP,  0, STD, 180,  50, 200, 160, 19, 3,               "Exhaust Recovery Loop:",  LEFT, -160, 5, 0, LEFT, 4, 5, ""
    EDIT, 15402, 15402, 0, 1, ELEC-GENERATOR, 0,          EXH-RCVR,  0, STD, 265,  75,  23,  55,  2, 3, "Frac Input Recoverable from Exhaust:",  LEFT, -245, 5, 1, LEFT, 4, 5, ""
   COMBO, 15403, 15403, 0, 1, ELEC-GENERATOR, 0,          JAC-LOOP,  0, STD, 180, 100, 200, 160, 19, 3,            "Engine-Jacket Gases Loop:",  LEFT, -160, 5, 0, LEFT, 4, 5, ""
    EDIT, 15404, 15404, 0, 1, ELEC-GENERATOR, 0,          JAC-RCVR,  0, STD, 265, 125,  23,  55,  2, 3, "Frac Inp Recvrbl from Engine-Jacket:",  LEFT, -245, 5, 1, LEFT, 4, 5, ""
   COMBO, 15405, 15405, 0, 1, ELEC-GENERATOR, 0,   RCVR-TRACK-LOOP,  0, STD, 180, 150, 200, 160, 19, 3,               "Thermal Tracking Mode:",  LEFT, -160, 5, 0, LEFT, 4, 5, ""

   LABEL, "Steam Loop", STD, LEFT, 420, 30, 1, 0, 0, 650, 15410, 3
   COMBO, 15410, 15410, 0, 1, ELEC-GENERATOR, 0,        STEAM-LOOP,  0, STD, 490,  50, 200, 160, 19, 3,                    "Loop:",  LEFT,  -70, 5, 0, LEFT, 4, 5, ""
    EDIT, 15411, 15411, 0, 1, ELEC-GENERATOR, 0,    STEAM-ENT-PRES, -1, STD, 575,  75,  23,  55,  1, 3, "Entering Steam Pressure:",  LEFT, -155, 5, 1, LEFT, 4, 5, ""
    EDIT, 15412, 15412, 0, 1, ELEC-GENERATOR, 0,     STEAM-SUPER-T, -1, STD, 575, 100,  23,  55,  1, 3,    "Superheat Above Sat.:",  LEFT, -155, 5, 1, LEFT, 4, 5, ""
    EDIT, 15413, 15413, 0, 1, ELEC-GENERATOR, 0,    STEAM-EXH-PRES, -1, STD, 575, 125,  23,  55,  1, 3,  "Exhaust Steam Pressure:",  LEFT, -155, 5, 1, LEFT, 4, 5, ""
    EDIT, 15414, 15414, 0, 1, ELEC-GENERATOR, 0,  STEAM-CONDENSATE, -1, STD, 575, 150,  23,  55,  1, 3, "Frac. Return Condensate:",  LEFT, -155, 5, 1, LEFT, 4, 5, ""

   LABEL, "Condenser Water Loop", STD, LEFT, 420, 210, 1, 0, 0, 650, 15406, 3
   COMBO, 15406, 15406, 0, 1, ELEC-GENERATOR, 0,           CW-LOOP,  0, STD, 490, 225, 200, 160, 19, 3,              "Loop:",  LEFT,  -70, 5, 0, LEFT, 4, 5, ""
   COMBO, 15407, 15407, 0, 1, ELEC-GENERATOR, 0,      CW-FLOW-CTRL,  0, STD, 490, 250,  80, 160, 19, 3,         "Flow Ctrl:",  LEFT,  -70, 5, 0, LEFT, 4, 5, ""
    EDIT, 15408, 15408, 0, 1, ELEC-GENERATOR, 0,             CW-DT, -1, STD, 575, 275,  23,  55,  1, 3,           "Delta T:",  LEFT, -155, 5, 1, LEFT, 4, 5, ""
    EDIT, 15409, 15409, 0, 1, ELEC-GENERATOR, 0,           CW-HEAD, -1, STD, 575, 300,  23,  55,  1, 3,              "Head:",  LEFT, -155, 5, 1, LEFT, 4, 5, ""


  ;******************************************
  ;  Electric Generator - Photo Voltaics
  ;******************************************
  TABPAGE, 3218, 32070, 1, 3, NOTIMP, " PV Array "

; SAC 3/30/03 - Implemented PV array stuff
     SUBTABPAGE, 3356, 32070, 1, 3, "   Array / Inverters   "

        CASE, ELEC-GENERATOR, 0, TYPE, -1, =, 1, 4
           LABEL, "PV Array", STD, LEFT, 30,  30, 1, 0, 0, 285, 17702, 3
           COMBO, 17702, 17702, 0, 1, ELEC-GENERATOR, 0,          PV-MODULE,  0, STD, 115,  50, 200, 170, 19, 3,                "PV Module:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "the photovoltaic module that comprises the array"
            EDIT, 17703, 17703, 0, 1, ELEC-GENERATOR, 0,     MODULES-SERIES,  0, STD, 195,  75,  23,  70,  0, 3,      "# of Series Modules:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the number of photovoltaic modules wired in series"
            EDIT, 17704, 17704, 0, 1, ELEC-GENERATOR, 0,   MODULES-PARALLEL,  0, STD, 195, 100,  23,  70,  0, 3,    "# of Parallel Modules:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the number of photovoltaic modules wired in parallel"

           LABEL, "Inverters", STD, LEFT, 30, 155, 1, 0, 0, 285, 17707, 3
            EDIT, 17707, 15388, 0, 1, ELEC-GENERATOR, 0,           CAPACITY,  0, STD, 195, 175,  23,  70,  3, 3,  "Capacity (per inverter):",  LEFT, -150, 5, 1, LEFT, 4, 5, "Nominal (rated) capacity per inverter"
            EDIT, 17708, 17708, 0, 1, ELEC-GENERATOR, 0,      NUM-INVERTERS,  0, STD, 195, 200,  23,  70,  0, 3,      "Number of Inverters:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the number of inverters that operate in parallel"
            EDIT, 17709, 17709, 0, 1, ELEC-GENERATOR, 0,   ELEC-INPUT-RATIO,  0, STD, 195, 225,  23,  70,  4, 3,     "Electric Input Ratio:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the ratio of direct-current input power to alternating-current output power"
           COMBO, 17710, 17710, 0, 1, ELEC-GENERATOR, 0,      INVERTER-CTRL,  0, STD, 165, 250, 200, 120, 19, 3,         "Inverter Control:",  LEFT, -120, 5, 0, LEFT, 4, 5, "the staging control mechanism as the load varies (only when more than one inverter is present)"

           LABEL, "Array Mount", STD, LEFT, 355,  30, 1, 0, 0, 640, 17713, 3
           COMBO, 17713, 17713, 0, 1, ELEC-GENERATOR, 0,         MOUNT-TYPE,  0, STD, 470,  50, 200, 170, 19, 3,               "Mount Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "the mounting configuration of the photovoltaic array"
           COMBO, 17714, 17714, 0, 1, ELEC-GENERATOR, 0,     BUILDING-SHADE,  0, STD, 470,  75, 200, 170, 19, 3,           "Building Shade:",  LEFT, -100, 5, 0, LEFT, 4, 5, "the shading surface on which the photovoltaic module(s) are mounted"
           COMBO, 17715, 17715, 0, 1, ELEC-GENERATOR, 0,      EXTERIOR-WALL,  0, STD, 470, 100, 200, 170, 19, 3,           "Ext. Wall/Roof:",  LEFT, -100, 5, 0, LEFT, 4, 5, "the exterior wall/roof surface on which the photovoltaic module(s) are mounted"
            EDIT, 17716, 17716, 0, 1, ELEC-GENERATOR, 0,     ARRAY-FRACTION,  0, STD, 470, 125,  23,  80,  3, 3,           "Array Fraction:",  LEFT, -100, 5, 1, LEFT, 4, 5, "the fraction of the shade, wall or roof surface that is covered by photovoltaic modules"
            EDIT, 17717, 17717, 0, 1, ELEC-GENERATOR, 0,       MOUNT-HEIGHT,  0, STD, 470, 150,  23,  80,  3, 3,             "Mount Height:",  LEFT, -100, 5, 1, LEFT, 4, 5, "the average distance between the back of the array and the surface to which it is mounted"
            EDIT, 17718, 17718, 0, 1, ELEC-GENERATOR, 0,      MOUNT-AZIMUTH,  0, STD, 470, 175,  23,  80,  2, 3,            "Mount Azimuth:",  LEFT, -100, 5, 1, LEFT, 4, 5, "the azimuth of the array rack, where 180° is due south, relative to the building coordinate system"
            EDIT, 17719, 17719, 0, 1, ELEC-GENERATOR, 0,         MOUNT-TILT,  0, STD, 470, 200,  23,  80,  2, 3,               "Mount Tilt:",  LEFT, -100, 5, 1, LEFT, 4, 5, "the tilt of the array rack, where 0° is horizontal (surface outward normal pointing straight up)"
        ENDCASE
        CASE, ELSE
           LABEL, "Photovoltaic Modules only apply to Electric Generators of type 'Photovoltaic Array'", ITALIC, CENTER, 350, 80, 1, 0, 0, 0, 0, 3
        ENDCASE

     SUBTABPAGE, 3357, 32070, 1, 3, "   Operating Limits / Conditions   "

        CASE, ELEC-GENERATOR, 0, TYPE, -1, =, 1, 4
           LABEL, "Array Ambient Conditions", STD, LEFT, 30,  30, 1, 0, 0, 315, 17725, 3
            EDIT, 17725, 17725, 0, 1, ELEC-GENERATOR, 0,  GND-REFLECTANCE,  0, STD, 170,  50,  23,  70,  3, 3,      "Ground Reflectance:",  LEFT, -125, 5, 1, LEFT, 4, 5, "the ground reflectance on the array rack"
; SAC 10/25/03 - Removed access to 3 no longer used keywords and added access to two new keywords
;            EDIT, 17726, 17726, 0, 1, ELEC-GENERATOR, 0,        WIND-COEF,  0, STD, 195,  75,  23,  80,  4, 3,        "Wind Coefficient:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the wind coefficient for the photovoltaic array"
;            EDIT, 17727, 17727, 0, 1, ELEC-GENERATOR, 0,         OFFSET-T,  0, STD, 195, 100,  23,  80,  2, 3,      "Offset Temperature:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the offset temperature for the photovoltaic array"
;            EDIT, 17728, 17728, 0, 1, ELEC-GENERATOR, 0,      CELL-T-COEF,  0, STD, 195, 125,  23,  80,  4, 3,  "Cell Temperature Coeff:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the coefficient that modifies the hourly operating cell temperature as a function of the irradiance, ambient temperature, and wind speed"
            EDIT, 17726, 17726, 0, 1, ELEC-GENERATOR, 0,      WIND-COEF-A,  0, STD, 170,  75,  23,  70,  4, 3,    "Wind Coefficient 'A':",  LEFT, -125, 5, 1, LEFT, 4, 5, "Coefficient determining upper temperature limit at low wind speeds"
            EDIT, 17727, 17727, 0, 1, ELEC-GENERATOR, 0,      WIND-COEF-B,  0, STD, 170, 100,  23,  70,  4, 3,    "Wind Coefficient 'B':",  LEFT, -125, 5, 1, LEFT, 4, 5, "Coefficient determining the rate that module T drops as wind increases"

           LABEL, "Operating Limits", STD, LEFT, 375,  30, 1, 0, 0, 640, 17731, 3
            EDIT, 17731, 17731, 0, 1, ELEC-GENERATOR, 0,   MIN-OPER-VOLTS,  0, STD, 540,  50,  23,  70,  2, 3,     "Minimum Input Volts:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the minimim input voltage below which the inverter will shut down"
            EDIT, 17732, 17732, 0, 1, ELEC-GENERATOR, 0,  MIN-TRACK-VOLTS,  0, STD, 540,  75,  23,  70,  2, 3,  "Minimun Tracking Volts:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the minimum input tracking voltage at which the inverter can operate efficiently"
            EDIT, 17733, 17733, 0, 1, ELEC-GENERATOR, 0,  MAX-TRACK-VOLTS,  0, STD, 540, 100,  23,  70,  2, 3,  "Maximum Tracking Volts:",  LEFT, -150, 5, 1, LEFT, 4, 5, "the maximum input tracking voltage at which the inverter can operate efficiently"
        ENDCASE
        CASE, ELSE
           LABEL, "Photovoltaic Modules only apply to Electric Generators of type 'Photovoltaic Array'", ITALIC, CENTER, 350, 80, 1, 0, 0, 0, 0, 3
        ENDCASE


  ;******************************************
  ; Electric Generator - Miscellaneous Page
  ;******************************************
  TABPAGE, 3217, 32070, 1, 3, NOTIMP, " Miscellaneous "

   LABEL, "Auxiliaries", STD, LEFT, 370, 30, 1, 0, 0, 600, 15380, 3
    EDIT, 15380, 15380, 0, 1, ELEC-GENERATOR, 0,            AUX-KW,  0, STD, 530,  50,  23,  50,  1, 3,            "Power:",  LEFT, -140, 5, 1, LEFT, 4, 5, "Auxiliary electric power consumption of the generator (e.g., control panels)"
   COMBO, 15382, 15382, 0, 1, ELEC-GENERATOR, 0,      AUX-SCHEDULE,  0, STD, 455,  75, 200, 150, 19, 3,         "Schedule:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "Schedule for Auxiliary Power consumption (set Auxiliary Mode to Scheduled to activate this)"
   COMBO, 15381, 15381, 0, 1, ELEC-GENERATOR, 0,          AUX-MODE,  0, STD, 455, 100, 120, 150, 19, 3,             "Mode:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "Always=all hours;When On=If gen. on;When Off=if gen. off;Scheduled=use Aux Schedule"
   COMBO, 15383, 15383, 0, 1, ELEC-GENERATOR, 0,         AUX-METER,  0, STD, 455, 125, 120, 150, 19, 3,            "Meter:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "Name of Electric Meter that tallies the electricity consumption of this generator's auxiliaries"


  ;******************************************
  ;  Not included in Electric Generator UI (at least for now)
  ;******************************************

  ;  ELEC-GENERATOR,  0,  COST-DATA,         "", 32070, 32070, 0,  2, "Name of a set of Materials Costs, which specifies first costs, maintenance costs, etc."
  ;  ELEC-GENERATOR,  0,  EQUIPMENT-REPORT,  "", 32070, 32070, 0,  2, "Whether or not a PS-H report is created for this generator"
  ;  ELEC-GENERATOR,  0,  PICTURE,           "", 32070, 32070, 0,  2, ""
  ;  ELEC-GENERATOR,  0,  DRAWING,           "", 32070, 32070, 0,  2, ""



; SAC 11/18/10 - added Condensing Unit tabbed dialog
; DEM 10/25/16 - updated Condensing unit dialog
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Condensing Unit Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

MODTABDLG, 3216, 32072, 1, 30, 30, 500, 780, 0, CONDENSING-UNIT, "Condensing Unit Properties", NOTIMP, 0, NOTIMP, 0
    COMBO, 14313, 14313, 0, 1, CONDENSING-UNIT, 0, NAME, -1, STD, 240,  15, 400, 180, 19, 3, "Currently Active Condensing Unit:",  LEFT, -200, 5, 0, LEFT, 4, 5, "List of all condensing units defined in project; also allows library retrieval and creation"
    STATIC, 1, CONDENSING-UNIT, 0, TYPE, 0, 0, 0, 440, 20, 150, STD, LEFT, "Type:  ",   "", 0, 3

     TABPAGE, 2506, 32072, 1, 3, NOTIMP," Basic Specs "
        EDIT, 14314, 14314, 0, 1, CONDENSING-UNIT, 0,              NAME, -1, STD, 170,  10,  23, 180, 32, 3,     "Condensing Unit Name:",  LEFT, -140, 5, 0, LEFT, 4, 5,"Name of condensing unit; right mouse quick menu options allow deleting, copying, linking and saving to library"
       COMBO, 14315, 14315, 0, 1, CONDENSING-UNIT, 0,              TYPE,  0, STD, 560,  10, 200, 150, 19, 3,                     "Type:",  LEFT, -100, 5, 0, LEFT, 4, 5,"VRF-HEAT-PUMP or VRF-HEAT-RECOVERY"
        EDIT, 14316, 14316, 0, 1, CONDENSING-UNIT, 0,       NUM-SYSTEMS,  0, STD, 180,  35,  23,  50,  1, 3, "Num systems (multiplier):",  LEFT, -160, 5, 0, LEFT, 4, 5,"Number of separate VRF systems represented by this CONDENSING-UNIT"
        EDIT, 14317, 14317, 0, 1, CONDENSING-UNIT, 0,    MAX-CAP/SYSTEM,  0, STD, 180,  60,  23,  90,  1, 3,           "Max cap/system:",  LEFT, -160, 5, 1, LEFT, 4, 5,"Max capacity per outdoor unit for autocalc of NUM-SYSTEMS"
        EDIT, 14318, 14318, 0, 1, CONDENSING-UNIT, 0,         NUM-UNITS,  0, STD, 180,  85,  23,  50,  1, 3,        "Num outdoor units:",  LEFT, -160, 5, 0, LEFT, 4, 5,"Number of outdoor units in one VRF system"


      LABEL, "Cooling Performance",  BOLD,  LEFT, 40, 115, 1, 0, 0, 345, 14318, 3
        EDIT, 14318, 14318, 0, 1, CONDENSING-UNIT, 0,  COOLING-CAPACITY,  0, STD, 185, 135,  23,  90,  1, 3,         "Cooling Capacity:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Cooling capacity in Btu/hr at rated conditions, i.e. rated saturated suction and saturated discharge temperatures."
        EDIT, 14319, 14319, 0, 1, CONDENSING-UNIT, 0,      COOLING-TONS,  0, STD, 185, 160,  23,  90,  1, 3,                     "Tons:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Cooling capacity in tons at rated conditions, alternate to Cool Capacity"
        EDIT, 14320, 14320, 0, 1, CONDENSING-UNIT, 0,  COOL-SIZING-RATI,  0, STD, 205, 185,  23,  70,  1, 3,        "Cool Sizing Ratio:",  LEFT, -140, 5, 1, LEFT, 4, 5,"Cooling sizing ratio if autosizing"
        EDIT, 14321, 14321, 0, 1, CONDENSING-UNIT, 0,       COOLING-EIR,  0, STD, 205, 210,  23,  70,  1, 3,         "Elec Input Ratio:",  LEFT, -140, 5, 1, LEFT, 4, 5,"The ratio of rated electric power to cooling capacity at rated conditions (i.e., the inverse of the cooling coefficient of performance (COP))"
        EDIT, 14322, 14322, 0, 1, CONDENSING-UNIT, 0,       COOLING-EER,  0, STD, 205, 235,  23,  70,  1, 3,         "Energy Eff Ratio:",  LEFT, -140, 5, 1, LEFT, 4, 5,"An alternative to Elec Input Ratio, the rated cooling capacity (Btu) divided by the rated power consumption in Watts"
        EDIT, 14323, 14323, 0, 1, CONDENSING-UNIT, 0,     COOLING-POWER,  0, STD, 205, 260,  23,  70,  1, 3,            "Cooling Power:",  LEFT, -140, 5, 1, LEFT, 4, 5,"An alternative to Cooling EIR, is the cooling-mode power consumption (compressor plus outdoor fan) at the rated conditions"
        EDIT, 14324, 14324, 0, 1, CONDENSING-UNIT, 0,    COOL-RATED-SST,  0, STD, 225, 285,  23,  50,  1, 3,        "Cooling Rated SST:",  LEFT, -160, 5, 1, LEFT, 4, 5,"Saturated suction temperature at which the cooling capacity and power (EIR) are specified."
        EDIT, 14325, 14325, 0, 1, CONDENSING-UNIT, 0,    COOL-RATED-SDT,  0, STD, 225, 310,  23,  50,  1, 3,        "Cooling Rated SDT:",  LEFT, -160, 5, 1, LEFT, 4, 5,"Saturated discharge temperature at which the cooling capacity and power (EIR) are specified."
        EDIT, 14326, 14326, 0, 1, CONDENSING-UNIT, 0,    COOL-RATED-ODB,  0, STD, 225, 335,  23,  50,  1, 3,       "Cooling Rated OADB:",  LEFT, -160, 5, 1, LEFT, 4, 5,"The outdoor drybulb temperature at which the cooling mode capacity and power are specified, either ARI or other."
        EDIT, 14327, 14327, 0, 1, CONDENSING-UNIT, 0,    DES-TARGET-SST,  0, STD, 225, 360,  23,  50,  1, 3,        "Design Target SST:",  LEFT, -160, 5, 1, LEFT, 4, 5,"Target saturated suction temperature at compressor for cooling design calcs; can be overridden by DES-MIN-SST or DES-MAX-SST specified for each indoor unit."

      LABEL, "Heating Performance",  BOLD,  LEFT, 350, 115, 1, 0, 0, 655, 19288, 3
        EDIT, 19288, 19288, 0, 1, CONDENSING-UNIT, 0,  HEATING-CAPACITY,  0, STD, 495, 135,  23,  90,  1, 3,         "Heating Capacity:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Heating capacity in Btu/hr at rated conditions, i.e. rated saturated suction and saturated discharge temperatures."
        EDIT, 19289, 19289, 0, 1, CONDENSING-UNIT, 0,  HEAT-SIZING-RATI,  0, STD, 515, 160,  23,  70,  1, 3,        "Heat Sizing Ratio:",  LEFT, -140, 5, 1, LEFT, 4, 5,"Heating sizing ratio if autosizing"
        EDIT, 19290, 19290, 0, 1, CONDENSING-UNIT, 0,    HEAT-RATED-SST,  0, STD, 535, 185,  23,  50,  1, 3,        "Heating Rated SST:",  LEFT, -160, 5, 1, LEFT, 4, 5,"Saturated suction temperature at which the heating capacity and power (EIR) are specified."
        EDIT, 19291, 19291, 0, 1, CONDENSING-UNIT, 0,    HEAT-RATED-SDT,  0, STD, 535, 210,  23,  50,  1, 3,        "Heating Rated SDT:",  LEFT, -160, 5, 1, LEFT, 4, 5,"Saturated discharge temperature at which the heating capacity and power (EIR) are specified."
        EDIT, 19292, 19292, 0, 1, CONDENSING-UNIT, 0,    HEAT-RATED-ODB,  0, STD, 535, 235,  23,  50,  1, 3,       "Heating Rated OADB:",  LEFT, -160, 5, 1, LEFT, 4, 5,"Rated outdoor drybulb in heating mode"
        EDIT, 19293, 19293, 0, 1, CONDENSING-UNIT, 0,    DES-TARGET-SDT,  0, STD, 535, 260,  23,  50,  1, 3,        "Design Target SDT:",  LEFT, -160, 5, 1, LEFT, 4, 5,"Target saturated discharge temperature at compressor for heating design calcs; can be overridden by DES-MIN-SST or DES-MAX-SST specified for each indoor unit."
        EDIT, 19294, 19294, 0, 1, CONDENSING-UNIT, 0,   DEFROST-MAX-ODB,  0, STD, 535, 285,  23,  50,  1, 3,         "Defrost Max OADB:",  LEFT, -160, 5, 1, LEFT, 4, 5,"No defrost above this outdoor air drybulb temperature."

     TABPAGE, 3379, 32072, 1, 3, NOTIMP," Performance Curves "
       COMBO, 19299, 19299, 0, 1, CONDENSING-UNIT, 0,      CAP-FSST&SDT,  0, STD, 205,  15, 300, 220, 19, 3,         "Cap f(SST, SDT) :",  LEFT, -140, 5, 1, LEFT, 4, 5,"Capacity adjustment curve for saturated suction and saturated discharge temperatures."
       COMBO, 19300, 19300, 0, 1, CONDENSING-UNIT, 0,      EIR-FSST&SDT,  0, STD, 205,  40, 300, 220, 19, 3,          "EIR f(SST, SDT):",  LEFT, -140, 5, 1, LEFT, 4, 5,"EIR adjustment curve for saturated suction and saturated discharge temperatures."
       COMBO, 19301, 19301, 0, 1, CONDENSING-UNIT, 0,          EIR-FPLR,  0, STD, 205,  65, 300, 220, 19, 3,            "EIR f(PLR,DT):",  LEFT, -140, 5, 1, LEFT, 4, 5,"EIR adjustment for PLR and (SDT-SST)."
       COMBO, 19302, 19302, 0, 1, CONDENSING-UNIT, 0,   COOL-CLOSS-FPLR,  0, STD, 205,  90, 300, 220, 19, 3,   "Cool f(Cycling on/off):",  LEFT, -140, 5, 1, LEFT, 4, 5,"Cooling mode cycling loss adjustment as function of run time fraction"
        EDIT, 19303, 19303, 0, 1, CONDENSING-UNIT, 0,    COOL-CLOSS-MIN,  0, STD, 205, 115,  23,  70,  1, 3,       "Cool Min Cycle PLR:",  LEFT, -140, 5, 1, LEFT, 4, 5,"The minimum cycling part load ratio used as input to cycling loss adjustment curve."
       COMBO, 19304, 19304, 0, 1, CONDENSING-UNIT, 0,   HEAT-CLOSS-FPLR,  0, STD, 205, 140, 300, 220, 19, 3,   "Heat f(Cycling on/off):",  LEFT, -140, 5, 1, LEFT, 4, 5,"Heating mode cycling loss adjustment as function of run time fraction"
        EDIT, 19305, 19305, 0, 1, CONDENSING-UNIT, 0,    HEAT-CLOSS-MIN,  0, STD, 205, 165,  23,  70,  1, 3,       "Heat Min cycle PLR:",  LEFT, -140, 5, 1, LEFT, 4, 5,"The minimum cycling part load ratio used as input to cycling loss adjustment curve."
        EDIT, 19306, 19306, 0, 1, CONDENSING-UNIT, 0,  MIN-UNLOAD-RATIO,  0, STD, 205, 190,  23,  70,  1, 3,         "Min unload ratio:",  LEFT, -140, 5, 1, LEFT, 4, 5,"Minimum unloading point of unit, hot gas bypas or cycling below"
        EDIT, 19307, 19307, 0, 1, CONDENSING-UNIT, 0,     MIN-HGB-RATIO,  0, STD, 205, 215,  23,  70,  1, 3,           "Min HGBP ratio:",  LEFT, -140, 5, 1, LEFT, 4, 5,"Point below which hot gas bypass starts"

     TABPAGE, 3380, 32072, 1, 3, NOTIMP," Controls "
       COMBO, 19317, 19306, 0, 1, CONDENSING-UNIT, 0,         UNIT-CTRL,  0, STD, 150,  10, 200, 150, 19, 3,             "Unit control:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Run-together or Run-staged"
       COMBO, 19318, 19307, 0, 1, CONDENSING-UNIT, 0,      CONTROL-ZONE,  0, STD, 150,  35, 300, 220, 19, 3,             "Control zone:",  LEFT, -130, 5, 1, LEFT, 4, 5,"For Heat Pump, the name of the zone that sets the heating/cooling mode. Default will poll all zones."
      LABEL, "Cooling Performance",  BOLD,  LEFT, 20, 65, 1, 0, 0, 390, 19328, 3
       COMBO, 19328, 19317, 0, 1, CONDENSING-UNIT, 0,          SST-CTRL,  0, STD, 170,  85, 200, 150, 19, 3,        "Cool Suction Ctrl:",  LEFT, -130, 5, 1, LEFT, 4, 5,"The method used to control the cooling-mode suction temperature."
        EDIT, 19329, 19329, 0, 1, CONDENSING-UNIT, 0,     MIN-SST-SETPT,  0, STD, 170, 110,  23,  70,  1, 3,            "Min SST reset:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Lower limit on saturated suction temperature at indoor coil when LOAD-RESET control is used."
        EDIT, 19330, 19330, 0, 1, CONDENSING-UNIT, 0,     MAX-SST-SETPT,  0, STD, 170, 135,  23,  70,  1, 3,            "Max SST reset:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Upper limit on saturated suction temperature at indoor coil when LOAD-RESET control is used."
      LABEL, "Heating Performance",  BOLD,  LEFT, 400, 65, 1, 0, 0, 690, 19340, 3
       COMBO, 19340, 19340, 0, 1, CONDENSING-UNIT, 0,          SDT-CTRL,  0, STD, 550,  85, 200, 150, 19, 3,      "Heat Discharge Ctrl:",  LEFT, -130, 5, 1, LEFT, 4, 5,"The method used to control the heating-mode condensing temperature"
        EDIT, 19341, 19341, 0, 1, CONDENSING-UNIT, 0,     MIN-SDT-SETPT,  0, STD, 550, 110,  23,  70,  1, 3,            "Min SDT reset:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Lower limit on saturated discharge temperature at indoor coil when LOAD-RESET control is used."
        EDIT, 19342, 19342, 0, 1, CONDENSING-UNIT, 0,     MAX-SDT-SETPT,  0, STD, 550, 135,  23,  70,  1, 3,            "Max SDT reset:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Upper limit on saturated discharge temperature at indoor coil when LOAD-RESET control is used."

     TABPAGE, 3381, 32072, 1, 3, NOTIMP," Outdoor Fan "
       COMBO, 19360, 19360, 0, 1, CONDENSING-UNIT, 0,       FAN-CONTROL,  0, STD, 120,  10, 200, 150, 19, 3,              "Fan Control:",  LEFT,  -90, 5, 1, LEFT, 4, 5,"FLOAT-TO-LIMIT indicates refrigerant temperature floats to min SDT or max SST based on outdoor temperature; LOAD-RESET indicates fan speed is reset in proportion to outdoor unit load."
        EDIT, 19361, 19361, 0, 1, CONDENSING-UNIT, 0,      COOL-MIN-SDT,  0, STD, 160,  35,  23,  70,  1, 3,             "Cool Min SDT:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Min SDT in cooling mode for Fan Control = FLOAT-TO-LIMIT"
        EDIT, 19362, 19362, 0, 1, CONDENSING-UNIT, 0,      HEAT-MAX-SST,  0, STD, 160,  60,  23,  70,  1, 3,             "Heat Max SDT:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Max SST in heating mode for Fan Control = FLOAT-TO-LIMIT"
        EDIT, 19363, 19363, 0, 1, CONDENSING-UNIT, 0,       FAN-AIRFLOW,  0, STD, 160,  85,  23,  70,  1, 3,           "Design Airflow:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Normalized air flow for outdoor unit, cfm per ton of rated cooling capacity."
        EDIT, 19364, 19364, 0, 1, CONDENSING-UNIT, 0,    FAN-POWER-FRAC,  0, STD, 160, 110,  23,  70,  1, 3,           "Fan Power Frac:",  LEFT, -130, 5, 1, LEFT, 4, 5,"The fraction of the total electrical power of the outdoor unit that is attributed to the fans."
        EDIT, 19365, 19365, 0, 1, CONDENSING-UNIT, 0,       FAN-PWR-EXP,  0, STD, 160, 135,  23,  70,  1, 3,            "Fan Power Exp:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Exponent that describes the power versus flow ralationship relationship of the outdoor fans when they modulate."
        EDIT, 19366, 19366, 0, 1, CONDENSING-UNIT, 0,   OUTDOOR-COIL-BF,  0, STD, 160, 160,  23,  70,  1, 3,          "Outdoor Coil BF:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Air bypass factor for outdoor coil"

     TABPAGE, 3388, 32072, 1, 3, NOTIMP," Pipe Losses "
        EDIT, 19376, 19376, 0, 1, CONDENSING-UNIT, 0,       PIPE-HEIGHT,  0, STD, 120,  10,  23,  70,  1, 3,              "Pipe Height:",  LEFT, -100, 5, 1, LEFT, 4, 5,"The typical height of the outdoor unit above the indoor units.  If the outdoor unit is lower than the indoor units, then this is a negative number."
      LABEL, "Leader Piping (outdoor unit to first branch)",  BOLD,  LEFT, 20, 40, 1, 0, 0, 380, 19377, 3
        EDIT, 19377, 19377, 0, 1, CONDENSING-UNIT, 0,        LDR-PIPE-L,  0, STD, 170,  60,  23,  70,  1, 3,       "Leader Pipe Length:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Length of leader pipe; i.e. distance from outdoor unit to first branch."
        EDIT, 19378, 19378, 0, 1, CONDENSING-UNIT, 0,     LDR-FITTING-L,  0, STD, 170,  85,  23,  70,  1, 3,    "Leader Fitting Length:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Eqivalent length of pipe fittings in leader refrigerant line."
        EDIT, 19379, 19379, 0, 1, CONDENSING-UNIT, 0,    LDR-HPG-PIPE-D,  0, STD, 170, 110,  23,  70,  1, 3,      "Leader HPG Pipe Dia:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Diameter of high pressure discharge pipe in leader refrigerant line. If not entered, the program will calculate a diameter based on common practice."
        EDIT, 19380, 19380, 0, 1, CONDENSING-UNIT, 0,    LDR-LPG-PIPE-D,  0, STD, 170, 135,  23,  70,  1, 3,      "Leader LPG Pipe Dia:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Diameter of low pressure suction pipe in leader refrigerant line. If not entered, the program will calculate a diameter based on common practice."
       COMBO, 19381, 19381, 0, 1, CONDENSING-UNIT, 0,      LDR-PIPE-LOC,  0, STD, 170, 160, 300, 150, 19, 3,     "Leader Pipe Location:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Location of refrigerant line: ZONE or OUTDOOR"
       COMBO, 19382, 19382, 0, 1, CONDENSING-UNIT, 0,     LDR-PIPE-ZONE,  0, STD, 170, 185, 300, 195, 19, 3,         "Leader Pipe Zone:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Name of building zone where refrigerant line is located."
      LABEL, "Header Piping (first branch to last branch)",  BOLD,  LEFT, 395, 40, 1, 0, 0, 730, 19383, 3
        EDIT, 19383, 19383, 0, 1, CONDENSING-UNIT, 0,        HDR-PIPE-L,  0, STD, 540,  60,  23,  70,  1, 3,       "Header Pipe Length:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Length of header pipe; first branch to last branch"
        EDIT, 19384, 19384, 0, 1, CONDENSING-UNIT, 0,     HDR-FITTING-L,  0, STD, 540,  85,  23,  70,  1, 3,    "Header Fitting Length:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Eqiv Len of fittings in header pipe"
        EDIT, 19385, 19385, 0, 1, CONDENSING-UNIT, 0,    HDR-HPG-PIPE-D,  0, STD, 540, 110,  23,  70,  1, 3,      "Header HPG Pipe Dia:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Diameter of high pressure discharge pipe in header refrigerant line. If not entered, the program will calculate a diameter based on common practice."
        EDIT, 19386, 19386, 0, 1, CONDENSING-UNIT, 0,    HDR-LPG-PIPE-D,  0, STD, 540, 135,  23,  70,  1, 3,      "Header LPG Pipe Dia:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Diameter of low pressure suction pipe in header refrigerant line. If not entered, the program will calculate a diameter based on common practice."
       COMBO, 19387, 19387, 0, 1, CONDENSING-UNIT, 0,      HDR-PIPE-LOC,  0, STD, 540, 160, 300, 150, 19, 3,     "Header Pipe Location:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Location of refrigerant line: ZONE or OUTDOOR"
       COMBO, 19388, 19388, 0, 1, CONDENSING-UNIT, 0,     HDR-PIPE-ZONE,  0, STD, 540, 185, 300, 195, 19, 3,         "Header Pipe Zone:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Name of building zone where refrigerant line is located."
        EDIT, 19389, 19389, 0, 1, CONDENSING-UNIT, 0,      HDR-AVG-FLOW,  0, STD, 540, 210,  23,  70,  1, 3,      "Avg. Flow in Header:",  LEFT, -130, 5, 1, LEFT, 4, 5,"The average refrigerant flow through the header as a ratio of the flow entering the header.  If branches are taken off the header at regular intervals, the value should be 0.5.  If branches are concentrated at the end of the line, then the value should be close to 1.0. "

     TABPAGE, 3389, 32072, 1, 3, NOTIMP," Miscellaneous "
      LABEL, "Overall VRF System Meter",  BOLD,  LEFT, 15, 10, 1, 0, 0, 450, 19399, 3
       COMBO, 19399, 19399, 0, 1, CONDENSING-UNIT, 0,        ELEC-METER,  0, STD, 160,  30, 300, 220, 19, 3,           "Electric meter:",  LEFT, -130, 5, 1, LEFT, 4, 5,"Electric meter for this equipment"
      LABEL, "Crankcase Heater",  BOLD,  LEFT, 15, 60, 1, 0, 0, 450, 19400, 3
        EDIT, 19400, 19400, 0, 1, CONDENSING-UNIT, 0,    CRANKCASE-HEAT,  0, STD, 170,  80,  23,  70,  1, 3,          "Crankcase Power:",  LEFT, -140, 5, 1, LEFT, 4, 5,"An alternative to CRANKCASE-EIR, is the electric power (Watts) used to heat the crankcase of the compressor(s)"
        EDIT, 19401, 19401, 0, 1, CONDENSING-UNIT, 0,     CRANKCASE-EIR,  0, STD, 170, 105,  23,  70,  1, 3,            "Crankcase EIR:",  LEFT, -140, 5, 1, LEFT, 4, 5,"Crankcase heater power as the ratio of crankcase power to rated cooling capacity, dimensionless"
       COMBO, 19402, 19402, 0, 1, CONDENSING-UNIT, 0,    CRANK-EIR-FPLR,  0, STD, 170, 130, 300, 220, 19, 3,     "Crankcase EIR-f(PLR):",  LEFT, -140, 5, 1, LEFT, 4, 5,"A curve that adjusts the crankcase heat as a function of the part-load ratio"
        EDIT, 19403, 19403, 0, 1, CONDENSING-UNIT, 0,   CRANKCASE-MAX-T,  0, STD, 170, 155,  23,  70,  1, 3,          "Crankcase Max T:",  LEFT, -140, 5, 1, LEFT, 4, 5,"The outside temperature above which the crankcase heater is always off"
      LABEL, "Auxiliary",  BOLD,  LEFT, 15, 185, 1, 0, 0, 450, 19404, 3
        EDIT, 19404, 19404, 0, 1, CONDENSING-UNIT, 0,         AUX-POWER,  0, STD, 150, 205,  23,  70,  1, 3,                "Aux Power:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Auxiliary electrical consumption, such as for controls"
       COMBO, 19405, 19405, 0, 1, CONDENSING-UNIT, 0,          AUX-MODE,  0, STD, 150, 230, 200, 150, 19, 3,                 "Aux Mode:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Operation mode when the AUX-KW is consumed"
       COMBO, 19406, 19406, 0, 1, CONDENSING-UNIT, 0,      AUX-SCHEDULE,  0, STD, 150, 255, 300, 220, 19, 3,             "Aux Schedule:",  LEFT, -120, 5, 1, LEFT, 4, 5,"When Aux Mode = Scheduled, the schedule (TYPE = FRACTION or MULTIPLIER) that varies the AUX-POWER"
       COMBO, 19407, 19407, 0, 1, CONDENSING-UNIT, 0,         AUX-METER,  0, STD, 150, 280, 300, 220, 19, 3,                "Aux Meter:",  LEFT, -120, 5, 1, LEFT, 4, 5,"Name of the meter that supplies the auxiliary energy"



; SAC 11/18/10 - replaced HEAT-EXCHANGER tabbed dialog (below) w/ CONDENSING-UNIT one (above) 
;  ;****************************************************************************************************************
;  ;****************************************************************************************************************
;  ;**
;  ;**     Heat Exchanger Dialog
;  ;**
;  ;****************************************************************************************************************
;  ;****************************************************************************************************************
; 
; ; MODDLG, 2506, 32072, 1, 100, 100, 400, 600, 0, "Heat Exchanger Data", NOTIMP, 0, NOTIMP, 0
;  MODTABDLG, 3216, 32072, 1, 30, 30, 435, 550, 0, HEAT-EXCHANGER, "Heat Exchanger Properties", NOTIMP, 0, NOTIMP, 0
;  
;  ;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
;     COMBO, 14313, 14313, 0, 1, HEAT-EXCHANGER, 0, NAME, -1, STD, 210,  15, 400, 180, 19, 3, "Currently Active Heat Exchanger:",  LEFT, -195, 5, 0, LEFT, 4, 5, "List of all heat exchangers defined in project; also allows library retrieval and creation"
;     STATIC, 1, HEAT-EXCHANGER, 0, TYPE, 0, 0, 0, 410, 20, 150, STD, LEFT, "Type:  ",   "", 0, 3
;  
;      ;******************************************
;      ; Heat Exchanger - Basic Specs Page
;      ;******************************************
;      TABPAGE, 2506, 32072, 1, 3, NOTIMP, " Basic Specifications "
;  
;         EDIT, 14314, 14314, 0, 1, HEAT-EXCHANGER, 0,              NAME, -1, STD, 135,  10,  23, 200, 32, 3,                "HX Name:",  LEFT, -105, 5, 0, LEFT, 4, 5, "Name of heat exchanger; right mouse quick menu options allow deleting, copying, linking and saving to library"
;        COMBO, 14315, 14315, 0, 1, HEAT-EXCHANGER, 0,              TYPE,  0, STD, 135,  35, 300, 150, 19, 3,                   "Type:",  LEFT, -105, 5, 0, LEFT, 4, 5, ""
;        COMBO, 14316, 14316, 0, 1, HEAT-EXCHANGER, 0,     CONFIGURATION,  0, STD, 135,  60, 110, 150, 19, 3,          "Configuration:",  LEFT, -105, 5, 0, LEFT, 4, 5, ""
; 
;         EDIT, 14317, 14317, 0, 1, HEAT-EXCHANGER, 0,          CAPACITY,  0, STD, 135, 105,  23,  75,  3, 3,               "Capacity:",  LEFT, -105, 5, 1, LEFT, 4, 5, ""
;         EDIT, 14318, 14318, 0, 1, HEAT-EXCHANGER, 0,        UA-PRODUCT,  0, STD, 135, 130,  23,  75,  1, 3,             "UA Product:",  LEFT, -105, 5, 1, LEFT, 4, 5, ""
;         EDIT, 14319, 14319, 0, 1, HEAT-EXCHANGER, 0,         INLETS-DT,  0, STD, 440, 105,  23,  50,  3, 3,          "Inlet Delta T:",  LEFT, -150, 5, 1, LEFT, 4, 5, ""
;         EDIT, 14320, 14320, 0, 1, HEAT-EXCHANGER, 0,         MAX-ERROR,  0, STD, 440, 130,  23,  50,  3, 3,  "Convergence Tolerance:",  LEFT, -150, 5, 1, LEFT, 4, 5, ""
; 
;        LABEL, "Supply-", STD, CENTER, 195, 177, 1, 0, 0, 0, 0, 3
;        LABEL,    "Side", STD, CENTER, 195, 193, 1, 0, 0, 0, 0, 3
;         EDIT, 14321, 14321, 0, 1, HEAT-EXCHANGER, 0,       SUPPLY-FLOW,  0, STD, 170, 210,  23,  50,  1, 3,                   "Flow:",  LEFT, -140, 5, 1, LEFT, 4, 5, ""
;         EDIT, 14322, 14322, 0, 1, HEAT-EXCHANGER, 0,   MAX-SUPPLY-FLOW,  0, STD, 170, 235,  23,  50,  2, 3,               "Max Flow:",  LEFT, -140, 5, 1, LEFT, 4, 5, ""
;         EDIT, 14323, 14323, 0, 1, HEAT-EXCHANGER, 0,   SUPPLY-FILM-RES,  0, STD, 170, 260,  23,  50,  1, 3,   "Film Resistance Frac:",  LEFT, -140, 5, 1, LEFT, 4, 5, ""
;         EDIT, 14324, 14324, 0, 1, HEAT-EXCHANGER, 0,   SUPPLY-FILM-EXP,  0, STD, 170, 285,  23,  50,  2, 3,      "Film Res Exponent:",  LEFT, -140, 5, 1, LEFT, 4, 5, ""
;         EDIT, 14510, 14510, 0, 1, HEAT-EXCHANGER, 0,  SUPPLY-PRES-DROP,  0, STD, 170, 310,  23,  50,  1, 3,          "Pressure Drop:",  LEFT, -140, 5, 1, LEFT, 4, 5, ""
; 
;       LABEL, "Demand-", STD, CENTER, 300, 177, 1, 0, 0, 0, 0, 3
;       LABEL,    "Side", STD, CENTER, 300, 193, 1, 0, 0, 0, 0, 3
;        EDIT, 14326, 14326, 0, 1, HEAT-EXCHANGER, 0,        DEMAND-FLOW,  0, STD, 275, 210,  23,  50,  1, 3,                        "",  LEFT,  -10, 5, 1, LEFT, 4, 5, ""
;        EDIT, 14327, 14327, 0, 1, HEAT-EXCHANGER, 0,    MAX-DEMAND-FLOW,  0, STD, 275, 235,  23,  50,  2, 3,                        "",  LEFT,  -10, 5, 1, LEFT, 4, 5, ""
;        EDIT, 14328, 14328, 0, 1, HEAT-EXCHANGER, 0,    DEMAND-FILM-RES,  0, STD, 275, 260,  23,  50,  1, 3,                        "",  LEFT,  -10, 5, 1, LEFT, 4, 5, ""
;        EDIT, 14329, 14329, 0, 1, HEAT-EXCHANGER, 0,    DEMAND-FILM-EXP,  0, STD, 275, 285,  23,  50,  2, 3,                        "",  LEFT,  -10, 5, 1, LEFT, 4, 5, ""
;        EDIT, 14511, 14511, 0, 1, HEAT-EXCHANGER, 0,   DEMAND-PRES-DROP,  0, STD, 275, 310,  23,  50,  1, 3,                        "",  LEFT,  -10, 5, 1, LEFT, 4, 5, ""



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Ground Loop HX - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

; MODTABDLG, 3138, 32082, 1, 100, 100, 310, 600, 0, "Ground HX Type:  ", GROUND-LOOP-HX, 0, TYPE, 0, 0, 0, "     Ground HX Name:  ", GROUND-LOOP-HX, 0, NAME, 0, 0, 0, ""
 MODTABDLG, 3138, 32082, 1, 100, 100, 470, 710, 0, GROUND-LOOP-HX, "Ground Loop Heat Exchanger Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 14497, 14497, 0, 1, GROUND-LOOP-HX, 0, NAME,  0, STD, 195,  15, 400, 240, 19, 3, "Currently Active Ground HX:",  LEFT, -170, 5, 0, LEFT, 4, 5, "List of all ground loop heat exchangers defined in project; also allows library retrieval and creation"
   STATIC, 1, GROUND-LOOP-HX, 0, TYPE, 0, 0, 0, 455, 20, 300, STD, LEFT, "Type:  ",   "", 0, 3

    ;******************************************
    ; Ground Loop HX - Basic Specifications
    ;******************************************
    TABPAGE, 3139, 32082, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 13142, 14497, 0, 1, GROUND-LOOP-HX, 0,        NAME, -1, STD, 105,  10,  23, 200, 32, 3,             "GHX Name:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Name of the ground loop heat exchanger; right mouse quick menu options allow deleting, copying, linking and saving to library"
      COMBO, 19150, 19150, 0, 1, GROUND-LOOP-HX, 0,        TYPE,  0, STD, 105,  35, 300, 200, 19, 3,             "GHX Type:",  LEFT,  -85, 5, 0, LEFT, 4, 5, ""

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 1
      LABEL, "Circulation Loop Assignment", STD, LEFT, 20, 80, 1, 0, 0, 305, 13143, 3
      COMBO, 13143, 19149, 0, 1, GROUND-LOOP-HX, 1, CIRCULATION-LOOP,  0, STD,  75, 100, 300, 230, 19, 3,                      "Loop:",  LEFT,  -40, 5, 0, LEFT, 4, 5, "Name of the attached Loop (the Loop's Type must be either WLHP or Condenser Water)"
      
      LABEL, "Ground Loop Temperature Schedule", STD, LEFT, 20, 155, 1, 0, 0, 305, 13144, 3
      COMBO, 13144, 14505, 0, 1, GROUND-LOOP-HX, 1,    LOOP-TEMP-SCH,  0, STD, 100, 175, 250, 205, 19, 3,                  "Schedule:",  LEFT,  -65, 5, 0, LEFT, 4, 5, "The (hourly) supply temperature of the Ground Loop Heat Exchanger"
      
;      EDIT, 13145, 13145, 0, 1, GROUND-LOOP-HX, 1,        COST-DATA,  0, STD, 120, 149,  23,  52,  0, 3,                      "Cost:",  LEFT,  -70, 5, 1, LEFT, 4, 5, ""
    ENDCASE   

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 2
      LABEL, "Ground Loop Configuration", STD, LEFT, 20, 80, 1, 0, 0, 265, 14393, 3
      COMBO, 14393, 14475, 0, 1, GROUND-LOOP-HX, 2,    CONFIGURATION,  0, STD, 125, 100, 300, 140, 19, 3,             "Configuration:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Configuration options vary by Ground Loop Heat Exchanger Type"
      
      LABEL, "Circulation Loop Assignment", STD, LEFT, 20, 155, 1, 0, 0, 265, 14394, 3
      COMBO, 14394, 19149, 0, 1, GROUND-LOOP-HX, 2, CIRCULATION-LOOP,  0, STD,  75, 175, 250, 190, 19, 3,                      "Loop:",  LEFT,  -40, 5, 0, LEFT, 4, 5, "Name of the attached Loop (the Loop's Type must be either WLHP or Condenser Water)"

      
      LABEL, "Pipe Properties", STD, LEFT, 20, 230, 1, 0, 0, 265, 14395, 3
       EDIT, 14395, 14325, 0, 1, GROUND-LOOP-HX, 2, PIPE-OUTSIDE-DIA,  0, STD, 150, 250,  23,  60,  2, 3,          "Outside Diameter:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Outside diameter of the U-tube or pipe"
       EDIT, 14396, 14471, 0, 1, GROUND-LOOP-HX, 2,  PIPE-INSIDE-DIA,  0, STD, 150, 275,  23,  60,  2, 3,           "Inside Diameter:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Inside diameter of the U-tube or pipe"
       EDIT, 14397, 14472, 0, 1, GROUND-LOOP-HX, 2,        PIPE-COND,  0, STD, 150, 300,  23,  60,  4, 3,              "Conductivity:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Thermal conductivity of the pipe"
;      EDIT, 14398, 14398, 0, 1, GROUND-LOOP-HX, 2,        COST-DATA,  0, STD, 140, 325,  23,  60,  0, 3,                      "Cost:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
       
      LABEL, "Vertical Well Field Properties", STD, LEFT, 390, 80, 1, 0, 0, 670, 14399, 3
       EDIT, 14399, 14476, 0, 1, GROUND-LOOP-HX, 2,            DEPTH,  0, STD, 580, 100,  23,  60,  1, 3,                        "Depth:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the ground surface and the bottom of the trench"
       EDIT, 14400, 14388, 0, 1, GROUND-LOOP-HX, 2,          SPACING,  0, STD, 580, 125,  23,  60,  1, 3,                      "Spacing:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the centerlines of each trench"
       EDIT, 14401, 14390, 0, 1, GROUND-LOOP-HX, 2,   U-TUBE-LEG-SEP,  0, STD, 580, 150,  23,  60,  1, 3,        "U-Tube Leg Separation:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the outer surfaces of the tubes"
       EDIT, 14402, 14391, 0, 1, GROUND-LOOP-HX, 2, FIELD-MULTIPLIER,  0, STD, 580, 175,  23,  60,  1, 3, "Num of Identical Well Fields:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Number of identical well fields"
    ENDCASE   

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 3
      LABEL, "Ground Loop Configuration", STD, LEFT, 20, 80, 1, 0, 0, 265, 13130, 3
      COMBO, 13130, 14475, 0, 1, GROUND-LOOP-HX, 3,    CONFIGURATION,  0, STD, 125, 100, 300, 140, 19, 3,             "Configuration:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Configuration options vary by Ground Loop Heat Exchanger Type"
      
      LABEL, "Pipe Properties", STD, LEFT, 20, 230, 1, 0, 0, 265, 13137, 3
       EDIT, 13137, 14325, 0, 1, GROUND-LOOP-HX, 3, PIPE-OUTSIDE-DIA,  0, STD, 150, 250,  23,  60,  2, 3,          "Outside Diameter:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Outside diameter of the U-tube or pipe"
       EDIT, 13140, 14471, 0, 1, GROUND-LOOP-HX, 3,  PIPE-INSIDE-DIA,  0, STD, 150, 275,  23,  60,  2, 3,           "Inside Diameter:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Inside diameter of the U-tube or "
       EDIT, 13141, 14472, 0, 1, GROUND-LOOP-HX, 3,        PIPE-COND,  0, STD, 150, 300,  23,  60,  4, 3,              "Conductivity:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Thermal conductivity of the pipe"
;      EDIT, 13142, 13142, 0, 1, GROUND-LOOP-HX, 3,        COST-DATA,  0, STD, 120, 251,  23,  60,  0, 3,                      "Cost:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""

      LABEL, "Circulation Loop Assignment", STD, LEFT, 20, 155, 1, 0, 0, 265, 14404, 3
      COMBO, 14404, 19149, 0, 1, GROUND-LOOP-HX, 4, CIRCULATION-LOOP,  0, STD,  75, 175, 250, 190, 19, 3,                         "Loop:",  LEFT,  -40, 5, 0, LEFT, 4, 5, "Name of the attached Loop (the Loop's Type must be either WLHP or Condenser Water)"
                 
      LABEL, "Trench Field Properties", STD, LEFT, 390, 80, 1, 0, 0, 670, 12012, 3
       EDIT, 12012, 14476, 0, 1, GROUND-LOOP-HX, 3,            DEPTH,  0, STD, 580, 100,  23,  60,  1, 3,                        "Depth:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the ground surface and the bottom of the trench"
       EDIT, 12059, 14388, 0, 1, GROUND-LOOP-HX, 3,          SPACING,  0, STD, 580, 125,  23,  60,  1, 3,                      "Spacing:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the centerlines of each trench"
       EDIT, 12523, 14478, 0, 1, GROUND-LOOP-HX, 3,    TRENCH-LENGTH,  0, STD, 580, 150,  23,  60,  1, 3,                "Trench Length:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The length of each trench "
       EDIT, 12525, 14479, 0, 1, GROUND-LOOP-HX, 3,    TRENCH-NUMBER,  0, STD, 580, 175,  23,  60,  1, 3, "Number of Identical Trenches:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The number of identical trenches"
       EDIT, 12808, 14480, 0, 1, GROUND-LOOP-HX, 3,    PIPE-VERT-SEP,  0, STD, 580, 200,  23,  60,  1, 3,     "Pipe Vertical Separation:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Vertical distance between centerlines of pipes (for pipes arranged vertically)"
       EDIT, 13047, 14481, 0, 1, GROUND-LOOP-HX, 3,   PIPE-HORIZ-SEP,  0, STD, 580, 225,  23,  60,  1, 3,   "Pipe Horizontal Separation:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Horizontal distance between centerlines of pipes (for pipes arranged horizontally)"
    ENDCASE   

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 4
      LABEL, "Ground Loop Configuration", STD, LEFT, 20, 80, 1, 0, 0, 265, 14403, 3
      COMBO, 14403, 14475, 0, 1, GROUND-LOOP-HX, 4,    CONFIGURATION,  0, STD, 125, 100, 300, 140, 19, 3,                "Configuration:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Configuration options vary by Ground Loop Heat Exchanger Type"
      
      LABEL, "Circulation Loop Assignment", STD, LEFT, 20, 155, 1, 0, 0, 265, 14404, 3
      COMBO, 14404, 19149, 0, 1, GROUND-LOOP-HX, 4, CIRCULATION-LOOP,  0, STD,  75, 175, 250, 190, 19, 3,                         "Loop:",  LEFT,  -40, 5, 0, LEFT, 4, 5, "Name of the attached Loop (the Loop's Type must be either WLHP or Condenser Water)"
      
      LABEL, "Pipe Properties", STD, LEFT, 20, 230, 1, 0, 0, 265, 14405, 3
       EDIT, 14405, 14325, 0, 1, GROUND-LOOP-HX, 4, PIPE-OUTSIDE-DIA,  0, STD, 150, 250,  23,  60,  2, 3,             "Outside Diameter:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Outside diameter of the U-tube or pipe"
       EDIT, 14406, 14471, 0, 1, GROUND-LOOP-HX, 4,  PIPE-INSIDE-DIA,  0, STD, 150, 275,  23,  60,  2, 3,              "Inside Diameter:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Inside diameter of the U-tube or "
       EDIT, 14407, 14472, 0, 1, GROUND-LOOP-HX, 4,        PIPE-COND,  0, STD, 150, 300,  23,  60,  4, 3,                 "Conductivity:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Thermal conductivity of the pipe"
;      EDIT, 14408, 14408, 0, 1, GROUND-LOOP-HX, 4,        COST-DATA,  0, STD, 120, 251,  23,  60,  0, 3,                         "Cost:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""
       
      LABEL, "Trench Field Properties", STD, LEFT, 390, 80, 1, 0, 0, 670, 14409, 3
       EDIT, 14409, 14476, 0, 1, GROUND-LOOP-HX, 4,            DEPTH,  0, STD, 580, 100,  23,  60,  1, 3,                        "Depth:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the ground surface and the bottom of the "
       EDIT, 14410, 14388, 0, 1, GROUND-LOOP-HX, 4,          SPACING,  0, STD, 580, 125,  23,  60,  1, 3,                      "Spacing:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the centerlines of each "
       EDIT, 14411, 14478, 0, 1, GROUND-LOOP-HX, 4,    TRENCH-LENGTH,  0, STD, 580, 150,  23,  60,  1, 3,                "Trench Length:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The length of each trench "
       EDIT, 14412, 14479, 0, 1, GROUND-LOOP-HX, 4,    TRENCH-NUMBER,  0, STD, 580, 175,  23,  60,  1, 3, "Number of Identical Trenches:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The number of identical trenches"
;      EDIT, 14413, 14480, 0, 1, GROUND-LOOP-HX, 4,    PIPE-VERT-SEP,  0, STD, 580, 200,  23,  60,  1, 3,     "Pipe Vertical Separation:",  LEFT, -175, 5, 1, LEFT, 4, 5, ""
;      EDIT, 14414, 14481, 0, 1, GROUND-LOOP-HX, 4,   PIPE-HORIZ-SEP,  0, STD, 580, 225,  23,  60,  1, 3,   "Pipe Horizontal Separation:",  LEFT, -175, 5, 1, LEFT, 4, 5, ""
       EDIT, 14415, 14492, 0, 1, GROUND-LOOP-HX, 4,  SLINKY-DIAMETER,  0, STD, 580, 200,  23,  60,  1, 3,          "'Slinky' Separation:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The diameter of the slinky coil"
       EDIT, 14417, 14493, 0, 1, GROUND-LOOP-HX, 4,     SLINKY-PITCH,  0, STD, 580, 225,  23,  60,  1, 3,               "'Slinky' Pitch:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The pitch of the slinky coil"
    ENDCASE   

; JJH 1/17/06 - GSHP mods - added new type
; SDG 3/21/13 – Hybrid mods – added SIZE-FIELD-MULT & CAPACITY-RATIO
    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 5
      LABEL, "Ground Loop Configuration", STD, LEFT, 20, 85, 1, 0, 0, 265, 17958, 3
      COMBO, 17959,     0, 0, 1, GROUND-LOOP-HX, 5,  G-FUNCTION-FROM,  0, STD, 125, 100, 300, 140, 19, 3,               "G Functions:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "G Functions can come from the predefined configuration in the library of from custom calculations"
       EDIT, 17960,     0, 0, 1, GROUND-LOOP-HX, 5,   G-FUNCTION-NUM,  0, STD, 188, 125,  23,  60,  1, 3,             "G Function ID:",  LEFT, -153, 5, 1, LEFT, 4, 5, "The integer number value of the custom G Function"
      COMBO, 18105, 18105, 0, 1, GROUND-LOOP-HX, 5,  SIZE-FIELD-MULT,  0, STD, 188, 150, 300,  60, 19, 3,     "Size Field Multiplier:",  LEFT,  -153, 5, 0, LEFT, 4, 5, "Apply rule-of-thumb to calculate the required number of identical well fields"
      COMBO, 17958, 14475, 0, 1, GROUND-LOOP-HX, 5,    CONFIGURATION,  0, STD, 125, 175, 300, 140, 19, 3,             "Configuration:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Configuration options vary by Ground Loop Heat Exchanger Type"
       EDIT, 18110, 18110, 0, 1, GROUND-LOOP-HX, 5,   CAPACITY-RATIO,  0, STD, 188, 200,  23,  60,  2, 3,            "Capacity Ratio:",  LEFT, -153, 5, 1, LEFT, 4, 5, "Fraction of load to be met by GLHX (normally specified only for hybrid system)"
      
      LABEL, "Pipe Properties", STD, LEFT, 20, 260, 1, 0, 0, 265, 17962, 3
       EDIT, 17962, 14325, 0, 1, GROUND-LOOP-HX, 5, PIPE-OUTSIDE-DIA,  0, STD, 150, 275,  23,  60,  2, 3,          "Outside Diameter:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Outside diameter of the U-tube or pipe"
       EDIT, 17963, 14471, 0, 1, GROUND-LOOP-HX, 5,  PIPE-INSIDE-DIA,  0, STD, 150, 300,  23,  60,  2, 3,           "Inside Diameter:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Inside diameter of the U-tube or pipe"
       EDIT, 17964, 14472, 0, 1, GROUND-LOOP-HX, 5,        PIPE-COND,  0, STD, 150, 325,  23,  60,  4, 3,              "Conductivity:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Thermal conductivity of the pipe"
       
;      EDIT, 17965, 14398, 0, 1, GROUND-LOOP-HX, 5,        COST-DATA,  0, STD, 570,  50,  23,  60,  0, 3,                      "Cost:",  LEFT, -110, 5, 1, LEFT, 4, 5, ""

      LABEL, "Circulation Loop Assignment", STD, LEFT, 380, 20, 1, 0, 0, 670, 17961, 3
      COMBO, 17961, 19149, 0, 1, GROUND-LOOP-HX, 5, CIRCULATION-LOOP,  0, STD, 440,  35, 300, 206, 19, 3,                      "Loop:",  LEFT,  -45, 5, 0, LEFT, 4, 5, "Name of the attached Loop (the Loop's Type must be either WLHP or Condenser Water)"
      
      LABEL, "Vertical Well Field Properties", STD, LEFT, 380, 85, 1, 0, 0, 670, 17966, 3
       EDIT, 17966, 14476, 0, 1, GROUND-LOOP-HX, 5,            DEPTH,  0, STD, 570, 100,  23,  60,  1, 3,                        "Depth:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the ground surface and the bottom of the well"
       EDIT, 17967,     0, 0, 1, GROUND-LOOP-HX, 5,    BOREHOLE-DIAM,  0, STD, 570, 125,  23,  60,  1, 3,            "Borehole diameter:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The diameter of the borehole of each indiviual well"
       EDIT, 17968,     0, 0, 1, GROUND-LOOP-HX, 5,       GROUT-COND,  0, STD, 570, 150,  23,  60,  2, 3,           "Grout Conductivity:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The conductivity of the grout used to fill the borehole"
       EDIT, 17969, 14388, 0, 1, GROUND-LOOP-HX, 5,          SPACING,  0, STD, 570, 175,  23,  60,  1, 3,                      "Spacing:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the centerlines of each borehole"
       EDIT, 17970, 14390, 0, 1, GROUND-LOOP-HX, 5,   U-TUBE-LEG-SEP,  0, STD, 570, 200,  23,  60,  1, 3,        "U-Tube Leg Separation:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Distance between the outer surfaces of the tubes"
       EDIT, 17971, 14391, 0, 1, GROUND-LOOP-HX, 5, FIELD-MULTIPLIER,  0, STD, 570, 225,  23,  60,  0, 3, "Num of Identical Well Fields:",  LEFT, -175, 5, 1, LEFT, 4, 5, "Number of identical well fields"
       
      LABEL, "Circulation Fluid Properties", STD, LEFT, 380, 260, 1, 0, 0, 670, 17972, 3
      COMBO, 17972,     0, 0, 1, GROUND-LOOP-HX, 5,             FLUID, 0, STD, 485, 275, 300, 162, 19, 3,                        "Fluid:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Configuration options vary by Ground Loop Heat Exchanger Type"
       EDIT, 17973,     0, 0, 1, GROUND-LOOP-HX, 5,  ANTI-FREEZE-CONC, 0, STD, 570, 300,  23,  60,  1, 3,    "Anti-Freeze Concentration:",  LEFT, -175, 5, 1, LEFT, 4, 5, "The diameter of the borehole of each indiviual well"

; UI control IDs 17974-17984 reserved for more/future controls here

    ENDCASE   


    ;******************************************
    ; Ground Loop HX - Ground Properties
    ;******************************************
    TABPAGE, 3140, 32082, 1, 3, NOTIMP, " Ground Properties "

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 1
      LABEL, "Ground Properties do not apply to 'Scheduled / Weather File' type of ground loops", ITALIC, CENTER, 350, 150, 1, 0, 0, 0, 0, 3
    ENDCASE   

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 2
      LABEL, "Soil Thermal Properties & History", STD,   LEFT,  20, 30, 1, 0, 0, 335, 14447, 3
       EDIT, 14447, 14447, 0, 1, GROUND-LOOP-HX, 2,    REF-GRND-TEMP,  0, STD, 225,  50,  23,  60,  1, 3,    "Undisturbed Avg Ground Temp:",  LEFT, -190, 5, 1, LEFT, 4, 5, "for horiz loop: undisturbed mean ground T;for vert wells: the undisturbed far-field ground T"
       EDIT, 14448, 14448, 0, 1, GROUND-LOOP-HX, 2, GRND-DIFFUSIVITY,  0, STD, 225,  75,  23,  60,  3, 3,     "Ground Thermal Diffusivity:",  LEFT, -190, 5, 1, LEFT, 4, 5, "Thermal diffusivity of the ground"
       EDIT, 14449, 14449, 0, 1, GROUND-LOOP-HX, 2,        GRND-COND,  0, STD, 225, 100,  23,  60,  3, 3,    "Ground Thermal Conductivity:",  LEFT, -190, 5, 1, LEFT, 4, 5, "Thermal conductivity of the ground"
       EDIT, 14450, 14499, 0, 1, GROUND-LOOP-HX, 2,     NUM-OF-YEARS,  0, STD, 225, 125,  23,  60,  0, 3,    "Years of Previous Operation:",  LEFT, -190, 5, 1, LEFT, 4, 5, "Number of years of previous operation using the typical load profile"

; SDG 11/27/2011 - Modified to remove DESIGN-HEAT-DAY, etc. and implement HISTORY-SETUP
      COMBO, 14451, 14451, 0, 1, GROUND-LOOP-HX, 2,    HISTORY-SETUP,  0, STD, 225, 150, 300, 120, 19, 3,       "History Simulation Years:",  LEFT, -190, 5, 0, LEFT, 4, 5, "Simulate all years in History, or a weighted subset"
       
    ENDCASE   

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 3
      LABEL, "Soil Thermal Properties & History", STD,   LEFT,  20, 30, 1, 0, 0, 350, 14453, 3
       EDIT, 14453, 14447, 0, 1, GROUND-LOOP-HX, 3,    REF-GRND-TEMP,  0, STD, 240,  50,  23,  60,  1, 3,    "Undisturbed Avg Ground Temp:",  LEFT, -205, 5, 1, LEFT, 4, 5, "for horiz loop: undisturbed mean ground T;for vert wells: the undisturbed far-field ground T"
       EDIT, 14454, 14448, 0, 1, GROUND-LOOP-HX, 3, GRND-DIFFUSIVITY,  0, STD, 240,  75,  23,  60,  3, 3,     "Ground Thermal Diffusivity:",  LEFT, -205, 5, 1, LEFT, 4, 5, "Thermal diffusivity of the ground"
       EDIT, 14455, 14449, 0, 1, GROUND-LOOP-HX, 3,        GRND-COND,  0, STD, 240, 100,  23,  60,  3, 3,    "Ground Thermal Conductivity:",  LEFT, -205, 5, 1, LEFT, 4, 5, "Thermal conductivity of the ground"
       EDIT, 14456, 14499, 0, 1, GROUND-LOOP-HX, 3,     NUM-OF-YEARS,  0, STD, 240, 125,  23,  60,  0, 3,    "Years of Previous Operation:",  LEFT, -205, 5, 1, LEFT, 4, 5, "Number of years of previous operation using the typical load profile"

; SDG 11/27/2011 - Modified to remove DESIGN-HEAT-DAY, etc. and implement HISTORY-SETUP
      COMBO, 14457, 14451, 0, 1, GROUND-LOOP-HX, 3,    HISTORY-SETUP,  0, STD, 240, 150, 300, 120, 19, 3,       "History Simulation Years:",  LEFT, -190, 5, 0, LEFT, 4, 5, "Simulate all years in History, or a weighted subset"
       EDIT, 14459, 14459, 0, 1, GROUND-LOOP-HX, 3,  GRND-YEAR-SWING,  0, STD, 240, 175,  23,  60,  1, 3, "Annual Surface Soil Temp Swing:",  LEFT, -205, 5, 1, LEFT, 4, 5, "The annual surface soil temperature swing"
       EDIT, 14460, 14460, 0, 1, GROUND-LOOP-HX, 3, GRND-PHASE-CONST,  0, STD, 240, 200,  23,  60,  1, 3, "Grnd Temp Swing Phase Constant:",  LEFT, -205, 5, 1, LEFT, 4, 5, "The phase constant (days) in ground temperature swing"
       
    ENDCASE   

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 4
      LABEL, "Soil Thermal Properties & History", STD,   LEFT,  20, 30, 1, 0, 0, 350, 14461, 3
       EDIT, 14461, 14447, 0, 1, GROUND-LOOP-HX, 4,    REF-GRND-TEMP,  0, STD, 240,  50,  23,  60,  1, 3,    "Undisturbed Avg Ground Temp:",  LEFT, -205, 5, 1, LEFT, 4, 5, "for horiz loop: undisturbed mean ground T;for vert wells: the undisturbed far-field ground T  "
       EDIT, 14462, 14448, 0, 1, GROUND-LOOP-HX, 4, GRND-DIFFUSIVITY,  0, STD, 240,  75,  23,  60,  3, 3,     "Ground Thermal Diffusivity:",  LEFT, -205, 5, 1, LEFT, 4, 5, "Thermal diffusivity of the ground"
       EDIT, 14463, 14449, 0, 1, GROUND-LOOP-HX, 4,        GRND-COND,  0, STD, 240, 100,  23,  60,  3, 3,    "Ground Thermal Conductivity:",  LEFT, -205, 5, 1, LEFT, 4, 5, "Thermal conductivity of the ground"
       EDIT, 14464, 14499, 0, 1, GROUND-LOOP-HX, 4,     NUM-OF-YEARS,  0, STD, 240, 125,  23,  60,  0, 3,    "Years of Previous Operation:",  LEFT, -205, 5, 1, LEFT, 4, 5, "Number of years of previous operation using the typical load profile"

; SDG 11/27/2011 - Modified to remove DESIGN-HEAT-DAY, etc. and implement HISTORY-SETUP
      COMBO, 14465, 14451, 0, 1, GROUND-LOOP-HX, 4,    HISTORY-SETUP,  0, STD, 240, 150, 300, 120, 19, 3,       "History Simulation Years:",  LEFT, -190, 5, 0, LEFT, 4, 5, "Simulate all years in History, or a weighted subset"
       EDIT, 14467, 14459, 0, 1, GROUND-LOOP-HX, 4,  GRND-YEAR-SWING,  0, STD, 240, 175,  23,  60,  1, 3, "Annual Surface Soil Temp Swing:",  LEFT, -205, 5, 1, LEFT, 4, 5, "The annual surface soil temperature swing"
       EDIT, 14468, 14460, 0, 1, GROUND-LOOP-HX, 4, GRND-PHASE-CONST,  0, STD, 240, 200,  23,  60,  1, 3, "Grnd Temp Swing Phase Constant:",  LEFT, -205, 5, 1, LEFT, 4, 5, "The phase constant (days) in ground temperature swing"
       
    ENDCASE   

; JJH 1/17/06 - GSHP mods - added new type
    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 5
      LABEL, "Soil Thermal Properties & History", STD,   LEFT,  20, 35, 1, 0, 0, 335, 17985, 3
       EDIT, 17985, 14447, 0, 1, GROUND-LOOP-HX, 5,    REF-GRND-TEMP,  0, STD, 225,  50,  23,  60,  1, 3,    "Undisturbed Avg Ground Temp:",  LEFT, -190, 5, 1, LEFT, 4, 5, "the undisturbed far-field ground T"
       EDIT, 17986,     0, 0, 1, GROUND-LOOP-HX, 5,     REF-GRND-ADJ,  0, STD, 225,  75,  23,  60,  1, 3,  "Undisturbed Ground Adjustment:",  LEFT, -190, 5, 1, LEFT, 4, 5, "the adjustment made to undisturbed far-field ground T for local weather conditions"
       EDIT, 17987, 14448, 0, 1, GROUND-LOOP-HX, 5, GRND-DIFFUSIVITY,  0, STD, 225, 100,  23,  60,  3, 3,     "Ground Thermal Diffusivity:",  LEFT, -190, 5, 1, LEFT, 4, 5, "Thermal diffusivity of the ground"
       EDIT, 17988, 14449, 0, 1, GROUND-LOOP-HX, 5,        GRND-COND,  0, STD, 225, 125,  23,  60,  3, 3,    "Ground Thermal Conductivity:",  LEFT, -190, 5, 1, LEFT, 4, 5, "Thermal conductivity of the ground"
       EDIT, 17989, 14499, 0, 1, GROUND-LOOP-HX, 5,     NUM-OF-YEARS,  0, STD, 225, 150,  23,  60,  0, 3,    "Years of Previous Operation:",  LEFT, -190, 5, 1, LEFT, 4, 5, "Number of years of previous operation using the typical load profile"

; SDG 11/27/2011 - Modified to remove DESIGN-HEAT-DAY, etc. and implement HISTORY-SETUP
      COMBO, 17990,     0, 0, 1, GROUND-LOOP-HX, 5,    HISTORY-SETUP,  0, STD, 225, 175, 300, 120, 19, 3,       "History Simulation Years:",  LEFT, -190, 5, 0, LEFT, 4, 5, "Simulate all years in History, or a weighted subset"
       

; UI control IDs 17993-17999 reserved for more/future controls here

    ENDCASE   


    ;******************************************
    ; Ground Loop HX - Attachments
    ;******************************************
    TABPAGE, 3141, 32082, 1, 3, NOTIMP, " Attachments "

   LABEL,                    "Loops",  STD,   LEFT,  20, 20, 1, 0, 0, 250, 14419, 3
   LABEL,  "Condenser Water or WLHP",  STD, CENTER, 173, 47, 1, 0, 0,   0, 14419, 3

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 1
; SAC 11/30/10 - added for DOE-2.2
      COMBO, 18007,     0, 0, 1, GROUND-LOOP-HX, 1, LOOP-SERIES-LOCN,  0, STD, 135,  65, 200, 105, 19, 3,     "Series Location:",  LEFT, -100, 5, 0, LEFT, 4, 5, "For GLHX equipment in series, whether at the upstream or downstream location"
      COMBO, 14418, 14504, 0, 1, GROUND-LOOP-HX, 1,          HX-PUMP,  0, STD, 105,  90, 200, 135, 19, 3,                "Pump:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Name of a Pump that circulates fluid through the ground loop"
      COMBO, 14419, 14419, 0, 1, GROUND-LOOP-HX, 1,     HX-FLOW-CTRL,  0, STD, 105, 115, 200, 135, 19, 3,           "Flow Ctrl:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Type of flow through the ground loop heat exchanger"
       EDIT, 14420, 14420, 0, 1, GROUND-LOOP-HX, 1,            HX-DT,  0, STD, 160, 140,  23,  60,  1, 3,             "Delta T:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Design temperature change of the fluid circulating through the ground loop"
       EDIT, 14421, 14421, 0, 1, GROUND-LOOP-HX, 1,          HX-HEAD,  0, STD, 160, 165,  23,  60,  1, 3,                "Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "The head loss through the ground loop piping at the design flow rate"
       EDIT, 14422, 14422, 0, 0, GROUND-LOOP-HX, 1,   HX-STATIC-HEAD,  0, STD, 160, 190,  23,  60,  1, 3,         "Static Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Static head loss of the ground loop"
       EDIT, 14423, 14423, 0, 1, GROUND-LOOP-HX, 1,      HX-MIN-FLOW,  0, STD, 160, 215,  23,  60,  1, 3,        "Minimum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Minimum allowable fraction of the design flow rate through the ground loop"
       EDIT, 14424, 14424, 0, 1, GROUND-LOOP-HX, 1,      HX-MAX-FLOW,  0, STD, 160, 240,  23,  60,  1, 3,        "Maximum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Ratio of the maximum allowable flow rate to the design flow rate"
    ENDCASE   

    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 2
; SAC 11/30/10 - added for DOE-2.2
      COMBO, 18006,     0, 0, 1, GROUND-LOOP-HX, 2, LOOP-SERIES-LOCN,  0, STD, 135,  65, 200, 105, 19, 3,     "Series Location:",  LEFT, -100, 5, 0, LEFT, 4, 5, "For GLHX equipment in series, whether at the upstream or downstream location"
      COMBO, 14425, 14504, 0, 1, GROUND-LOOP-HX, 2,          HX-PUMP,  0, STD, 105,  90, 200, 135, 19, 3,                "Pump:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Name of a Pump that circulates fluid through the ground loop"
      COMBO, 14426, 14419, 0, 1, GROUND-LOOP-HX, 2,     HX-FLOW-CTRL,  0, STD, 105, 115, 200, 135, 19, 3,           "Flow Ctrl:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Type of flow through the ground loop heat exchanger"
       EDIT, 14427, 14420, 0, 1, GROUND-LOOP-HX, 2,            HX-DT,  0, STD, 160, 140,  23,  60,  1, 3,             "Delta T:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Design temperature change of the fluid circulating through the ground loop"
       EDIT, 14428, 14421, 0, 1, GROUND-LOOP-HX, 2,          HX-HEAD,  0, STD, 160, 165,  23,  60,  1, 3,                "Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "The head loss through the ground loop piping at the design flow rate"
       EDIT, 14429, 14422, 0, 0, GROUND-LOOP-HX, 2,   HX-STATIC-HEAD,  0, STD, 160, 190,  23,  60,  1, 3,         "Static Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Static head loss of the ground loop"
       EDIT, 14430, 14423, 0, 1, GROUND-LOOP-HX, 2,      HX-MIN-FLOW,  0, STD, 160, 215,  23,  60,  1, 3,        "Minimum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Minimum allowable fraction of the design flow rate through the ground loop"
       EDIT, 14431, 14424, 0, 1, GROUND-LOOP-HX, 2,      HX-MAX-FLOW,  0, STD, 160, 240,  23,  60,  1, 3,        "Maximum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Ratio of the maximum allowable flow rate to the design flow rate"
; SDG 3/20/13 Hybrid GLHP 
       EDIT, 18106, 18106, 0, 1, GROUND-LOOP-HX, 2,   HX-BYPASS-FLOW,  0, STD, 160, 265,  23,  60,  1, 3,        "Bypass Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Fraction of the total loop flow that will be conditioned by the HX, but that is bypassed around the HX"
    ENDCASE   
                                                                                    
    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 3
; SAC 11/30/10 - added for DOE-2.2
      COMBO, 18005,     0, 0, 1, GROUND-LOOP-HX, 3, LOOP-SERIES-LOCN,  0, STD, 135,  65, 200, 105, 19, 3,     "Series Location:",  LEFT, -100, 5, 0, LEFT, 4, 5, "For GLHX equipment in series, whether at the upstream or downstream location"
      COMBO, 14432, 14504, 0, 1, GROUND-LOOP-HX, 3,          HX-PUMP,  0, STD, 105,  90, 200, 135, 19, 3,                "Pump:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Name of a Pump that circulates fluid through the ground loop"
      COMBO, 14433, 14419, 0, 1, GROUND-LOOP-HX, 3,     HX-FLOW-CTRL,  0, STD, 105, 115, 200, 135, 19, 3,           "Flow Ctrl:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Type of flow through the ground loop heat exchanger"
       EDIT, 14434, 14420, 0, 1, GROUND-LOOP-HX, 3,            HX-DT,  0, STD, 160, 140,  23,  60,  1, 3,             "Delta T:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Design temperature change of the fluid circulating through the ground loop"
       EDIT, 14435, 14421, 0, 1, GROUND-LOOP-HX, 3,          HX-HEAD,  0, STD, 160, 165,  23,  60,  1, 3,                "Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "The head loss through the ground loop piping at the design flow rate"
       EDIT, 14436, 14422, 0, 0, GROUND-LOOP-HX, 3,   HX-STATIC-HEAD,  0, STD, 160, 190,  23,  60,  1, 3,         "Static Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Static head loss of the ground loop"
       EDIT, 14437, 14423, 0, 1, GROUND-LOOP-HX, 3,      HX-MIN-FLOW,  0, STD, 160, 215,  23,  60,  1, 3,        "Minimum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Minimum allowable fraction of the design flow rate through the ground loop"
       EDIT, 14438, 14424, 0, 1, GROUND-LOOP-HX, 3,      HX-MAX-FLOW,  0, STD, 160, 240,  23,  60,  1, 3,        "Maximum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Ratio of the maximum allowable flow rate to the design flow rate"
; SDG 3/20/13 Hybrid GLHP 
       EDIT, 18107, 18107, 0, 1, GROUND-LOOP-HX, 3,   HX-BYPASS-FLOW,  0, STD, 160, 265,  23,  60,  1, 3,        "Bypass Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Fraction of the total loop flow that will be conditioned by the HX, but that is bypassed around the HX"
    ENDCASE   
                                                                                    
    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 4
; SAC 11/30/10 - added for DOE-2.2
      COMBO, 18004,     0, 0, 1, GROUND-LOOP-HX, 4, LOOP-SERIES-LOCN,  0, STD, 135,  65, 200, 105, 19, 3,     "Series Location:",  LEFT, -100, 5, 0, LEFT, 4, 5, "For GLHX equipment in series, whether at the upstream or downstream location"
      COMBO, 14439, 14504, 0, 1, GROUND-LOOP-HX, 4,          HX-PUMP,  0, STD, 105,  90, 200, 135, 19, 3,                "Pump:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Name of a Pump that circulates fluid through the ground loop"
      COMBO, 14440, 14419, 0, 1, GROUND-LOOP-HX, 4,     HX-FLOW-CTRL,  0, STD, 105, 115, 200, 135, 19, 3,           "Flow Ctrl:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Type of flow through the ground loop heat exchanger"
       EDIT, 14441, 14420, 0, 1, GROUND-LOOP-HX, 4,            HX-DT,  0, STD, 160, 140,  23,  60,  1, 3,             "Delta T:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Design temperature change of the fluid circulating through the ground loop"
       EDIT, 14442, 14421, 0, 1, GROUND-LOOP-HX, 4,          HX-HEAD,  0, STD, 160, 165,  23,  60,  1, 3,                "Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "The head loss through the ground loop piping at the design flow rate"
       EDIT, 14443, 14422, 0, 0, GROUND-LOOP-HX, 4,   HX-STATIC-HEAD,  0, STD, 160, 190,  23,  60,  1, 3,         "Static Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Static head loss of the ground loop"
       EDIT, 14444, 14423, 0, 1, GROUND-LOOP-HX, 4,      HX-MIN-FLOW,  0, STD, 160, 215,  23,  60,  1, 3,        "Minimum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Minimum allowable fraction of the design flow rate through the ground loop"
       EDIT, 14445, 14424, 0, 1, GROUND-LOOP-HX, 4,      HX-MAX-FLOW,  0, STD, 160, 240,  23,  60,  1, 3,        "Maximum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Ratio of the maximum allowable flow rate to the design flow rate"
; SDG 3/20/13 Hybrid GLHP 
       EDIT, 18108, 18108, 0, 1, GROUND-LOOP-HX, 4,   HX-BYPASS-FLOW,  0, STD, 160, 265,  23,  60,  1, 3,        "Bypass Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Fraction of the total loop flow that will be conditioned by the HX, but that is bypassed around the HX"
    ENDCASE   

; JJH 1/17/06 - GSHP mods - added new type
    CASE,  GROUND-LOOP-HX,  0, TYPE,  -1,  =, 1, 5
; SAC 11/30/10 - added for DOE-2.2
      COMBO, 19284,     0, 0, 1, GROUND-LOOP-HX, 5, LOOP-SERIES-LOCN,  0, STD, 135,  65, 200, 105, 19, 3,     "Series Location:",  LEFT, -100, 5, 0, LEFT, 4, 5, "For GLHX equipment in series, whether at the upstream or downstream location"
      COMBO, 18201, 14504, 0, 1, GROUND-LOOP-HX, 5,          HX-PUMP,  0, STD, 105,  90, 200, 135, 19, 3,                "Pump:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Name of a Pump that circulates fluid through the ground loop"
      COMBO, 18202, 14419, 0, 1, GROUND-LOOP-HX, 5,     HX-FLOW-CTRL,  0, STD, 105, 115, 200, 135, 19, 3,           "Flow Ctrl:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "Type of flow through the ground loop heat exchanger"
       EDIT, 18203, 14420, 0, 1, GROUND-LOOP-HX, 5,            HX-DT,  0, STD, 160, 140,  23,  60,  1, 3,             "Delta T:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Design temperature change of the fluid circulating through the ground loop"
       EDIT, 18204, 14421, 0, 1, GROUND-LOOP-HX, 5,          HX-HEAD,  0, STD, 160, 165,  23,  60,  1, 3,                "Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "The head loss through the ground loop piping at the design flow rate"
       EDIT, 18205, 14422, 0, 0, GROUND-LOOP-HX, 5,   HX-STATIC-HEAD,  0, STD, 160, 190,  23,  60,  1, 3,         "Static Head:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Static head loss of the ground loop"
       EDIT, 18206, 14423, 0, 1, GROUND-LOOP-HX, 5,      HX-MIN-FLOW,  0, STD, 160, 215,  23,  60,  1, 3,        "Minimum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Minimum allowable fraction of the design flow rate through the ground loop"
       EDIT, 18207, 14424, 0, 1, GROUND-LOOP-HX, 5,      HX-MAX-FLOW,  0, STD, 160, 240,  23,  60,  1, 3,        "Maximum Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Ratio of the maximum allowable flow rate to the design flow rate"
; SDG 3/20/13 Hybrid GLHP 
       EDIT, 18109, 18109, 0, 1, GROUND-LOOP-HX, 5,   HX-BYPASS-FLOW,  0, STD, 160, 265,  23,  60,  1, 3,        "Bypass Flow:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Fraction of the total loop flow that will be conditioned by the HX, but that is bypassed around the HX"
    ENDCASE   

; FROM PD1's DataWnd
;        BUTTON, 10380, 10354, 0, 1, 2500, STD, 653, 132, 21, 65, "Pump...", "Attached Pump Data"



 ;********************************************************************
 ;********************************************************************
 ;**
 ;**     G-FUNCTIONS Dialog Box
 ;**
 ;********************************************************************
 ;********************************************************************

; JJH 1/17/06 - GSHP mods
 MODTABDLG, 3367,   0, 1,  0,  0, 390, 710, 0, G-FUNCTIONS, "G Function Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 18210,  0, 0, 1, G-FUNCTIONS, 0, NAME,  0, STD, 300,  15, 400, 250, 19, 3, "Currently Active G-Function:",  LEFT, -170, 5, 0, LEFT, 4, 5, "List of all polygons defined in project; also allows library retrieval and creation"

    ;******************************************
    ; G Functions - Basic Specs Page
    ;******************************************
    TABPAGE, 3368,  0, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 18211,     0,    0, 1,  G-FUNCTIONS, 0,        NAME, -1, STD, 140,  10,  23, 270, 32, 3,  "G Function Name:",  LEFT, -110, 5, 0, LEFT, 4, 5, "Name of G Function"

     SPREAD, 18212,     0, 0, 1, 0,  PowerDOE,    0, GFuncSpread,  0, STD,  30,  50, 250, 650, 19, 3,  "",                  LEFT,    0, 0, 0, LEFT, 0, 0, ""



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Pumps Dialog Box
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODDLG, 2500, 2005, 1, 100, 100, 380, 530, 0, "Pump Data", NOTIMP, 0, NOTIMP, 0 
MODTABDLG, 3147, 2005, 1, 100, 100, 470, 710, 0, PUMP, "Pump Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 19157, 682, 0, 1, PUMP, 0, NAME,  0, STD, 300,  15, 400, 250, 19, 3, "Currently Active Pump:",  RIGHT, -10, 5, 0, LEFT, 4, 5, "List of all pumps defined in project; also allows library retrieval and creation"

    ;******************************************
    ; Pump - Basic Specifications Page
    ;******************************************
    TABPAGE, 3148, 2005, 1, 3, NOTIMP, " Basic Specifications "

;   LINE,  10, 46, 510, 46, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
;  COMBO, 19157,   682, 0, 1, PUMP, 0,             NAME, -1, STD, 210,  13, 200, 220, 19, 3, "Currently Active Pump:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all pumps defined in project; also allows library retrieval"	
;  COMBO, 14798,   682, 0, 1, PUMP, 0,          NAMEOPT,  0, STD,  70,  60, 136, 180, 19, 3,                  "Pump:",  LEFT,  -50, 5, 0, LEFT, 4, 5, "Name of pump; options allow renaming, deleting, copying, linking, save to library"

; SAC 7/25/06 - adjusted ALL control Y positions and added C-MTR-ENCL-TYPE - per KJM e-mail of 6/27/06
    EDIT, 14798,   682, 0, 1, PUMP, 0,             NAME, -1, STD, 120,   5,  23, 190, 32, 3,             "Pump Name:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "Name of pump; right mouse quick menu options allow deleting, copying, linking and saving to library"

    EDIT, 12856, 12856, 0, 1, PUMP, 0,           NUMBER, -1, STD, 160,  35,  23,  70,  0, 3,       "Number of Pumps:",  LEFT, -130, 5, 0, LEFT, 4, 5, "Number of identical pumps attached to this equipment"
    EDIT, 12852, 12852, 0, 1, PUMP, 0,             HEAD, -1, STD, 160,  60,  23,  70,  1, 3,       "Head (per pump):",  LEFT, -130, 5, 1, LEFT, 4, 5, "Design pressure rise of the fluid across the pump (when the pump is running)"
    EDIT, 12853, 12853, 0, 1, PUMP, 0,             FLOW, -1, STD, 160,  85,  23,  70,  1, 3,       "Flow (per pump):",  LEFT, -130, 5, 1, LEFT, 4, 5, "Design flowrate of the pump"
    EDIT, 12854, 12854, 0, 1, PUMP, 0,       HEAD-RATIO, -1, STD, 160, 110,  23,  70,  2, 3,            "Head Ratio:",  LEFT, -130, 5, 1, LEFT, 4, 5, "When autosizing, DOE-2 oversizes the head imparted by the Loop Pump using this ratio"
    EDIT, 12855, 12855, 0, 1, PUMP, 0,       FLOW-RATIO, -1, STD, 160, 135,  23,  70,  2, 3,            "Flow Ratio:",  LEFT, -130, 5, 1, LEFT, 4, 5, "When autosizing, DOE-2 oversizes the design flowrate of the Loop Pump using this ratio"
    EDIT, 12823,   993, 0, 1, PUMP, 0,   PUMP-MAX-RATIO, -1, STD, 160, 160,  23,  70,  2, 3,        "Max Pump Ratio:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Maximum flow rate that the pump can impart (as a fraction of the design pump flow rate)"
    EDIT, 12887,   678, 0, 1, PUMP, 0,       HEAD-SETPT, -1, STD, 160, 185,  23,  70,  2, 3,         "Head Setpoint:",  LEFT, -130, 5, 1, LEFT, 4, 5, "The design setpoint of the pump's differential head pressure sensor"
;    EDIT, 12888, 32063, 0, 1, PUMP, 0, HEAD-SETPT-RATIO, -1, STD, 160, 210,  23,  70,  2, 3,   "Head Setpoint Ratio:",  LEFT, -130, 5, 1, LEFT, 4, 5, ""   ; SAC 11/24/10 - removed

   COMBO, 12863, 12863, 0, 1, PUMP, 0,  PUMP-HEAD-FFLOW, -1, STD, 160, 260, 200, 150, 19, 3,     "Pump Head f(flow):",  LEFT, -130, 5, 1, LEFT, 4, 5, "Cubic Curve Fit: the head imparted by the pump as a function of the flow rate"
   COMBO, 12864, 12864, 0, 1, PUMP, 0,    PUMP-HP-FFLOW, -1, STD, 160, 285, 200, 150, 19, 3,    "Pump Power f(flow):",  LEFT, -130, 5, 1, LEFT, 4, 5, "Cubic Curve Fit: the horsepower input to the pump as a function of the flow rate"
    EDIT, 12824,   994, 0, 1, PUMP, 0,   PUMP-POWER-EXP, -1, STD, 160, 310,  23,  70,  2, 3,     "Pump Pwr Exponent:",  LEFT, -130, 5, 1, LEFT, 4, 5, "How pump horsepower varies with speed (when all other parameters obey the ideal pump laws)"

   COMBO, 12889, 63025, 0, 1, PUMP, 0,       ELEC-METER, -1, STD, 500,  35, 200, 150, 19, 3,        "Electric Meter:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption of the pump"
    EDIT, 12857, 12857, 0, 1, PUMP, 0,          PUMP-KW, -1, STD, 500,  60,  23,  70,  2, 3,            "Pump Power:",  LEFT, -115, 5, 1, LEFT, 4, 5, "The design power consumption of the pump"
    EDIT, 12858, 12858, 0, 1, PUMP, 0,        MOTOR-EFF, -1, STD, 500,  85,  23,  70,  2, 3,      "Motor Efficiency:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Efficiency of the pump motor (default is based on Motor Class & Pump Power)"
    EDIT, 12859, 12859, 0, 1, PUMP, 0,         MECH-EFF, -1, STD, 500, 110,  23,  70,  2, 3,       "Mech Efficiency:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Mechanical Efficiency of the pump impeller"
    EDIT, 12860, 12860, 0, 1, PUMP, 0,        MIN-SPEED, -1, STD, 500, 135,  23,  70,  2, 3,         "Minimum Speed:",  LEFT, -115, 5, 1, LEFT, 4, 5, "The lower speed of a 2-speed pump, or the minimum speed of a variable-speed pump"
   COMBO, 12861, 12861, 0, 1, PUMP, 0,      MOTOR-CLASS, -1, STD, 500, 160, 120, 150, 19, 3,           "Motor Class:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Efficiency classification of the motor (High & Premium Efficiency are based on NEMA standards)"
   COMBO, 12862, 12862, 0, 1, PUMP, 0,         CAP-CTRL, -1, STD, 500, 185, 120, 150, 19, 3,      "Capacity Control:",  LEFT, -115, 5, 0, LEFT, 4, 5, "A pump can 'ride its curve' (if a 2 way valve exists), be Two Speed, or be Variable Speed"

; SAC 10/24/00 - Compliance keyword
   LABEL, "Compliance Inputs", STD, LEFT, 385, 218, 1, 0, 0, 650, 15484, 1
   COMBO, 15615,     0, 0, 1, PUMP, 0,     C-MOTOR-TYPE, -1, STD, 500, 235, 300, 150, 19, 1,            "Motor Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "The type of pump motor"
; SAC 7/25/06 - added C-MTR-ENCL-TYPE - per KJM e-mail of 6/27/06
   COMBO, 18240, 18240, 0, 1, PUMP, 0,  C-MTR-ENCL-TYPE, -1, STD, 500, 235, 300, 150, 19, 1,        "Enclosure Type:",  LEFT, -100, 5, 0, LEFT, 4, 5, "The type of motor enclosure for the pump"
   COMBO, 15616,     0, 0, 1, PUMP, 0,    C-MOTOR-SPEED, -1, STD, 500, 260, 300, 150, 19, 1,           "Motor Speed:",  LEFT, -100, 5, 0, LEFT, 4, 5, "The synchronous speed of the pump motor"
; DEM 10/26/12 new keyword for motor subtype to identify T24 level
  COMBO, 17205,     0, 0, 1, PUMP, 0,     C-MOTOR-SUB, -1, STD, 500, 285, 300, 180, 19, 1,            "Motor Subtype:",  LEFT, -100, 5, 0, LEFT, 4, 5, "Motor phase and subtype classification"
    EDIT, 15617,     0, 0, 1, PUMP, 0,      C-DRIVE-EFF, -1, STD, 500, 310,  23,  70,  3, 1,      "Drive Efficiency:",  LEFT, -100, 5, 1, LEFT, 4, 5, "The pump drive efficiency"
    EDIT, 15618,     0, 0, 1, PUMP, 0,         C-NOM-HP, -1, STD, 500, 335,  23,  70,  2, 1,            "Nominal HP:",  LEFT, -100, 5, 1, LEFT, 4, 5, "The total pump motor nominal (nameplate) horsepower"
    EDIT, 15619,     0, 0, 1, PUMP, 0,            C-BHP, -1, STD, 500, 360,  23,  70,  2, 1,              "Brake HP:",  LEFT, -100, 5, 1, LEFT, 4, 5, "The brake horsepower demand of the pump motor"


;    BUTTON,     8,     8, 0, 0,    1, STD, 295, 320, 24, 65, 3, "Default", "" 	
;    BUTTON,     1,     1, 0, 1,    1, STD, 370, 320, 24, 65, 3, "OK", "" 	
;    BUTTON,     2,     2, 0, 0,    2, STD, 445, 320, 24, 65, 3, "Cancel", "" 	



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Thermal Storage - Tabbed Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODTABDLG, 3120, 32071, 1, 100, 100, 470, 710, 0, "Thermal Storage Type:  ", THERMAL-STORAGE, 0, TYPE, 0, 0, 0, "     Name:  ", THERMAL-STORAGE, 0, NAME, 0, 0, 0, ""
 MODTABDLG, 3120, 32071, 1, 100, 100, 470, 710, 0, THERMAL-STORAGE, "Thermal Storage Properties", NOTIMP, 0, NOTIMP, 0
 
   COMBO, 15375, 15375, 0, 1, THERMAL-STORAGE, 0, NAME,  0, STD, 225,  15, 400, 250, 19, 3, "Currently Active Thermal Storage:",  LEFT, -202, 5, 0, LEFT, 4, 5, "List of all thermal storage components defined in project; also allows library retrieval and creation"
   STATIC, 1, THERMAL-STORAGE, 0, TYPE, 0, 0, 0, 500, 20, 300, STD, LEFT, "Type:  ",   "", 0, 3

 ;******************************************
 ; Thermal Storage - Basic Specifications Sheet
 ;******************************************
  TABPAGE, 3121, 32071, 1, 3, NOTIMP, " Basic Specifications "

      EDIT, 15376, 15376, 0, 1, THERMAL-STORAGE, 0,        NAME, -1, STD,  95,  10,  23, 200, 32, 3,             "TES Name:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Name of thermal storage component; right mouse quick menu options allow deleting, copying, linking and saving to library"
     COMBO, 15377, 15377, 0, 1, THERMAL-STORAGE, 0,        TYPE,  0, STD, 370,  10, 300, 125, 19, 3,                 "Type:",  RIGHT,  -5, 5, 0, LEFT, 4, 5, ""

    CASE,  THERMAL-STORAGE,  0, TYPE,  -1,  =, 1, 1
      LABEL,  "Loop Assignments", STD, LEFT, 20, 70, 1, 0, 0, 220, 19140, 3
      COMBO, 19140, 12528, 0, 1, THERMAL-STORAGE, 1,        CHRG-LOOP,  0, STD,  75,  90, 200, 145, 19, 3,              "Charge:",  LEFT,  -55, 5, 0, LEFT, 4, 5, "Name of the loop that charges the tank (more than one storage tank per loop is allowed)"
      COMBO, 19141, 12076, 0, 1, THERMAL-STORAGE, 1,       DCHRG-LOOP,  0, STD,  75, 115, 200, 145, 19, 3,            "Dischrge:",  LEFT,  -55, 5, 0, LEFT, 4, 5, "Name of the loop the tank discharges to (only one tank can dicharge to any particular loop)"
      COMBO, 19142, 19142, 0, 1, THERMAL-STORAGE, 1,      FREEZE-LOOP,  0, STD,  75, 140, 200, 145, 19, 3,              "Freeze:",  LEFT,  -55, 5, 0, LEFT, 4, 5, "Name of Hot Water or Two Pipe loop that heats a Cold Water Tank to prevent freezing "
; SAC 12/1/10 - added for DOE-2.3
      COMBO, 18003,     0, 0, 1, THERMAL-STORAGE, 1, DCHRG-SERIES-LOC,  0, STD, 115, 165, 275, 105, 19, 3,     "Series Location:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "For thermal storage discharge equipment in series, whether at the upstream or downstream location"
    ENDCASE   
    CASE,  THERMAL-STORAGE,  0, TYPE,  -1,  =, 1, 2
      LABEL,  "Loop Assignments", STD, LEFT, 20, 70, 1, 0, 0, 220, 19171, 3
      COMBO, 19171, 12528, 0, 1, THERMAL-STORAGE, 2,        CHRG-LOOP,  0, STD,  75,  90, 200, 145, 19, 3,              "Charge:",  LEFT,  -55, 5, 0, LEFT, 4, 5, "Name of the loop that charges the tank (more than one storage tank per loop is allowed)"
      COMBO, 19172, 12076, 0, 1, THERMAL-STORAGE, 2,       DCHRG-LOOP,  0, STD,  75, 115, 200, 145, 19, 3,            "Dischrge:",  LEFT,  -55, 5, 0, LEFT, 4, 5, "Name of the loop the tank discharges to (only one tank can dicharge to any particular loop)"
; SAC 12/1/10 - added for DOE-2.3
      COMBO, 18002,     0, 0, 1, THERMAL-STORAGE, 2, DCHRG-SERIES-LOC,  0, STD, 115, 140, 275, 105, 19, 3,     "Series Location:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "For thermal storage discharge equipment in series, whether at the upstream or downstream location"
    ENDCASE   

    LABEL, "Charge/Discharge Operations", STD, LEFT, 20, 215, 1, 0, 0, 220, 13235, 3
    COMBO, 13235, 12079, 0, 1, THERMAL-STORAGE, 0,          CHRG-SCH,  0, STD,  80, 235, 200, 140, 19, 3,            "Chrg Sch:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "Name of an on/off schedule that defines when the tank is allowed to be charged"
     EDIT, 13247, 12078, 0, 1, THERMAL-STORAGE, 0,    MAX-DCHRG-RATE,  0, STD, 125, 260,  23,  55,  1, 3,      "Max Dchrg Rate:",  LEFT, -105, 5, 1, LEFT, 4, 5, "maximum rate at which the storage tank can discharge (i.e., supply the loop)"
     EDIT, 13259, 12666, 0, 1, THERMAL-STORAGE, 0,     MAX-CHRG-RATE,  0, STD, 125, 285,  23,  55,  1, 3,       "Max Chrg Rate:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Maximum rate at which the storage tank can charge"
     EDIT, 13357, 13357, 0, 1, THERMAL-STORAGE, 0,   DELAY-CHRG-HOUR,  0, STD, 125, 310,  23,  55,  1, 3,        "Delay Charge:",  LEFT, -105, 5, 1, LEFT, 4, 5, "The latest hour (while Charge Schedule is ON) by which the tank should be fully charged"
     EDIT, 13358, 13358, 0, 1, THERMAL-STORAGE, 0,      INITIAL-CHRG,  0, STD, 125, 335,  23,  55,  1, 3,      "Initial Charge:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Fraction of the tank's Capacity that is stored at the start of the simulation"

   
    LABEL, "Equipment Capacity", STD, LEFT, 265, 70, 1, 0, 0, 435, 13110, 3
     EDIT, 13110, 12876, 0, 1, THERMAL-STORAGE, 0,          CAPACITY,  0, STD, 345,  90,  23,  60,  1, 3,            "Capacity:",  LEFT,  -80, 5, 1, LEFT, 4, 5, "Net thermal storage capacity of the tank"
     EDIT, 13155, 12944, 0, 1, THERMAL-STORAGE, 0,    CAPACITY-RATIO,  0, STD, 365, 115,  23,  40,  1, 3,      "Capacity Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Tank is sized to meet this multiplied by 1 hour's design loop load (if Capacity not specified)"
   
    LABEL, "Operating Temperatures", STD, LEFT, 265, 215, 1, 0, 0, 435, 13359, 3
     EDIT, 13359, 12945, 0, 1, THERMAL-STORAGE, 0,            BASE-T,  0, STD, 365, 235,  23,  50,  1, 3,           "Base Temp:",  LEFT, -100, 5, 1, LEFT, 4, 5, "When tank reaches this temperature, no more storage is possible"
     EDIT, 13403, 12946, 0, 1, THERMAL-STORAGE, 0,           T-RANGE,  0, STD, 365, 260,  23,  50,  1, 3,          "Temp Range:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Temperature range between the fully charged and fully discharged state"
     EDIT, 13648, 12947, 0, 1, THERMAL-STORAGE, 0,            CHRG-T,  0, STD, 365, 285,  23,  50,  1, 3,         "Charge Temp:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Temperature at which the tank is fully charged (may force loop to exceed its setpoint temp)"
     EDIT, 13681, 13681, 0, 1, THERMAL-STORAGE, 0,          FREEZE-T,  0, STD, 365, 310,  23,  50,  1, 3,         "Freeze Temp:",  LEFT, -100, 5, 1, LEFT, 4, 5, "Temperature at which the tank storage medium freezes"

                                                                                                                                                     
    LABEL, "Losses", STD, LEFT, 480, 70, 1, 0, 0, 675, 13268, 3
     EDIT, 13268, 13268, 0, 1, THERMAL-STORAGE, 0,   LOSS-COEFICIENT,  0, STD, 585,  90,  23,  46,  3, 3,     "Loss Coefficient:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Thermal losses of the tank, per degree temperature difference between tank and its Location "
    COMBO, 13694, 12793, 0, 1, THERMAL-STORAGE, 0,          LOCATION,  0, STD, 565, 115, 120, 110, 19, 3,             "Location:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Outdoor=Losses based on ouside air drybulb; Zone=Losses based on temp of Zone Name"
    COMBO, 13712, 12874, 0, 1, THERMAL-STORAGE, 0,         ZONE-NAME,  0, STD, 565, 140, 120, 110, 19, 3,            "Zone Name:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Name of the space the storage tank is in (used only if Location = Zone)"
   
;   COMBO, 13786, 12077, 0, 1, THERMAL-STORAGE, 0,         COST-DATA,  0, STD, 445, 145, 120, 137, 19, 3,                 "Cost:",  LEFT,  -45, 5, 0, LEFT, 4, 5, "Name of a set of Materials Costs"


 ;******************************************
 ; Thermal Storage - Performance Curves
 ;******************************************
  TABPAGE, 3122, 32071, 1, 3, NOTIMP, " Performance Curves "
    
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;  
; Commented out for first release:
;   COMBO, 14051, 14051, 0, 1, THERMAL-STORAGE, 0,        SIM-ALGORITM,  0, STD, 429, 22, 120, 137, 21, 3,      "Simulation Algorithm", RIGHT, 416, 5, 0, LEFT, 4, 5, ""
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;  
  
   LABEL,  "Discharge Rate",    STD, CENTER, 190, 18, 1, 0, 0, 0, 14021, 3
   COMBO, 14021, 14021, 0, 1, THERMAL-STORAGE, 0,       DCHRG-RATE-FHOURS,  0, STD, 105, 38, 200, 180, 19, 3,    "f(hours):",  LEFT,  -75, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: discharge rate as function of length of time tank has been discharging"
   
   LABEL, "Charge Rate",        STD, CENTER, 390, 18, 1, 0, 0, 0, 14049, 3
   COMBO, 14049, 14049, 0, 1, THERMAL-STORAGE, 0,        CHRG-RATE-FHOURS,  0, STD, 305, 38, 200, 180, 19, 3,             "",  LEFT,   -5, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: charge rate as function of length of time tank has been charging"
    
   LABEL, "Charge Temperature", STD, CENTER, 590, 18, 1, 0, 0, 0, 14050, 3
   COMBO, 14050, 14050, 0, 1, THERMAL-STORAGE, 0,           CHRG-T-FHOURS,  0, STD, 505, 38, 200, 180, 19, 3,             "",  LEFT,   -5, 5, 0, LEFT, 4, 5, "Quadratic Curve Fit: charge temp as function of length of time tank has been charged"


 ;******************************************
 ; Thermal Storage - Miscellaneous Sheet
 ;******************************************
  TABPAGE, 3123, 32071, 1, 3, NOTIMP, " Miscellaneous "
  
   LABEL, "Auxiliaries", STD, LEFT, 370, 25, 1, 0, 0, 580, 13790, 3
    EDIT, 13790, 13033, 0, 1, THERMAL-STORAGE, 0,           AUX-KW,  0, STD, 510,  45,  23,  50,  1, 3,           "Power:", LEFT, -120, 5, 1, LEFT, 4, 5, "Auxiliary electric power consumption of the thermal storage device"
   COMBO, 13791, 13037, 0, 1, THERMAL-STORAGE, 0,     AUX-SCHEDULE,  0, STD, 455,  70, 200, 125, 19, 3,        "Schedule:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Schedule for Auxiliary Power consumption (set Auxiliary Mode to Scheduled to activate this)"
   COMBO, 13805, 13057, 0, 1, THERMAL-STORAGE, 0,         AUX-MODE,  0, STD, 455,  95, 120, 125, 19, 3,            "Mode:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Always=all hours;When On=If on;When Off=if off;Scheduled=use Aux Schedule"
   COMBO, 13806, 13062, 0, 1, THERMAL-STORAGE, 0,        AUX-METER,  0, STD, 455, 120, 120, 125, 19, 3,           "Meter:", LEFT,  -65, 5, 0, LEFT, 4, 5, "Name of the Electric Meter that tallies the electricity consumption of the auxiliaries"

  

;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;
; CONVERSION STEPS:
;
; 1. Add BDL Command Edited (or NOTIMP) before Caption for dialogs, tabbed dialogs & tabbed dialog pages
;
; 2. Change tabbed dialog size from "310, 610" to "470, 710"
;
; 3. Change label and units label coordinates to be in relation to top-left and top-right corners of the control
;
; 4. Add two properties to each LABEL -> right shadowline X coord & ID of associated UI control (both 0 for none)
;    - also remove trailing ':'s from labels with shadowline extensions
;
; 5. Switch all ComboBox "Height of edit portion of control" values from 21 to 19
;
; 6. Switch all Edit "Height" values from 21 to 23
;
; 7. Switch all font settings of "ITALIC_UND" to "STD"
;
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 

 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Steam Meter Tab Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODTABDLG, 3004, 32077, 1,  50, 100, 360, 600, 0, "Steam Meter: ", STEAM-METER, 0, NAME, 0, 0, 0, "", NOTIMP, 0, NOTIMP, 0 
 MODTABDLG, 3004, 32077, 1, 100, 100, 470, 710, 0, STEAM-METER, "Steam Meter Properties", NOTIMP, 0, NOTIMP, 0 

   COMBO, 15378, 15378, 0, 1, STEAM-METER, 0, NAME,  0, STD, 290,  15, 400, 250, 19, 3, "Currently Active Steam Meter:",  LEFT, -185, 5, 0, LEFT, 4, 5, "List of all steam meter components defined in project; also allows library retrieval and creation"

   ;*****************************************
   ; Basic Specifications 
   ;*****************************************
   TABPAGE, 3102, 32077, 1, 3, NOTIMP, " Basic Specifications "
 
      EDIT, 14106, 14106, 0, 1, STEAM-METER, 0,             NAME,  0, STD, 145,  10,  23, 200, 32, 3,   "Steam Meter Name:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Name of steam meter component; right mouse quick menu options allow deleting, copying, linking and saving to library"

     LABEL, "Loop Assignment", STD, LEFT, 20, 60, 1, 0, 0, 205, 19135, 3
     COMBO, 19135, 19076, 0, 1, STEAM-METER, 0, CIRCULATION-LOOP,  0, STD,  65,  80, 250, 140, 19, 3,               "Loop:",  LEFT,  -45, 5, 0, LEFT, 4, 5, "Name of the Loop this meter is attached to (Loop Type must be compatible)"
; SAC 11/30/10 - added for DOE-2.3
     COMBO, 18001,     0, 0, 1, STEAM-METER, 0, LOOP-SERIES-LOCN,  0, STD,  95, 105, 275, 110, 19, 3,        "Series Locn:",  LEFT,  -75, 5, 0, LEFT, 4, 5, "For a steam meter in series, whether at the upstream or downstream location"
   
     LABEL, "Billing Unit Thermal Value", STD, LEFT, 20, 165, 1, 0, 0, 205, 14123, 3
      EDIT, 14123, 14110, 0, 1, STEAM-METER, 0,      ENERGY/UNIT,  0, STD,  80, 185,  23,  80,  0, 3,           "Btu/Unit:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Number of Btus per billing unit for this meter (e.g. 100,000 for therms)"
   
     LABEL, "Billing Units Labels", STD, LEFT, 20, 240, 1, 0, 0, 160, 14124, 3
      EDIT, 14124, 14124, 0, 1, STEAM-METER, 0,       UNIT-INDEX,  0, STD,  80, 260,  23,  80,  0, 3,             "Energy:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the billing unit, used to convert english/metric units"
      EDIT, 14125, 14125, 0, 1, STEAM-METER, 0,   DEM-UNIT-INDEX,  0, STD,  80, 285,  23,  80,  0, 3,             "Demand:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the maximum demand billing unit"
   
     LABEL, "Equipment Capacity", STD, LEFT, 245, 60, 1, 0, 0, 425, 14126, 3
      EDIT, 14126, 14108, 0, 1, STEAM-METER, 0,         CAPACITY,  0, STD, 315,  80,  23,  70,  0, 3,           "Capacity:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "Capacity of the meter, defaults to product of Loop Capacity & the meter's Capacity Ratio"
      EDIT, 14127, 14109, 0, 1, STEAM-METER, 0,   CAPACITY-RATIO,  0, STD, 345, 105,  23,  40,  0, 3,     "Capacity Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "If the meter Capacity is undefined, it is set to the product of this and the loop capacity"
   
     LABEL, "Equipment Efficiency", STD, LEFT, 470, 60, 1, 0, 0, 675, 14128, 3
      EDIT, 14128, 14111, 0, 1, STEAM-METER, 0,  SOURCE-SITE-EFF,  0, STD, 585,  80,  23,  50,  3, 3, "Source-to-Site Eff:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Fraction of total energy used at the utility source that arrives at the site boundary"
   
     LABEL, "Heat Exchanger", STD, LEFT, 470, 135, 1, 0, 0, 675, 14129, 3
      EDIT, 14129, 14112, 0, 1, STEAM-METER, 0,          HX-HEAD,  0, STD, 585, 155,  23,  50,  0, 3,     "Heat Exch Head:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Pressure drop through the meter's heat exchanger (if one exists)"
      EDIT, 14130, 14113, 0, 1, STEAM-METER, 0,   HX-STATIC-HEAD,  0, STD, 585, 180,  23,  50,  0, 3,     "HX Static Head:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Static pressure drop through the meter's heat exchanger (zero for almost all systems)"

 
   ;*****************************************
   ; Direct Loads 
   ;*****************************************
   TABPAGE, 3103, 32077, 1, 3, NOTIMP, " Direct Loads "
   
; SAC 9/27/04 - Added access to existing INTERIOR-EU and new EXTERIOR-EU keywords
   LABEL, "Misc. Direct Loads, Interior", STD, LEFT,  25, 30, 1, 0, 0, 515, 11600, 3
     SPREAD, 11600, 11600, 0, 1, 0, PowerDOE, 0, SteamMtrInt,  0, STD,  40,  50, 120, 475, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     
   LABEL, "Misc. Direct Loads, Exterior", STD, LEFT,  25, 195, 1, 0, 0, 515, 11601, 3
     SPREAD, 11601, 11601, 0, 1, 0, PowerDOE, 0, SteamMtrExt,  0, STD,  40, 215, 120, 475, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""

 
 
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     CHW Meter Tab Dialog
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
 
; MODTABDLG, 3104, 3104, 1,  50, 100, 360, 600, 0, "Chilled Water Meter: ", CHW-METER, 0, NAME, 0, 0, 0, "", NOTIMP, 0, NOTIMP, 0 
 MODTABDLG, 3104, 3104, 1,  50, 100, 470, 710, 0, CHW-METER, "Chilled Water Meter Properties", NOTIMP, 0, NOTIMP, 0 

   COMBO, 15379, 15379, 0, 1, CHW-METER, 0, NAME,  0, STD, 300,  15, 400, 250, 19, 3, "Currently Active Chilled Water Meter:",  LEFT, -225, 5, 0, LEFT, 4, 5, "List of all steam meter components defined in project; also allows library retrieval and creation"

   ;*****************************************
   ; Basic Specifications 
   ;*****************************************
   TABPAGE, 3105, 3104, 1, 3, NOTIMP, " Basic Specifications "

      EDIT, 14114, 14114, 0, 1, CHW-METER, 0,             NAME,  0, STD, 145,  10,  23, 200, 32, 3,      "CHW Meter Name:",  LEFT, -125, 5, 1, LEFT, 4, 5, "Name of steam meter component; right mouse quick menu options allow deleting, copying, linking and saving to library"

     LABEL, "Loop Assignment", STD, LEFT, 20, 60, 1, 0, 0, 205, 19137, 3
     COMBO, 19137, 19136, 0, 1, CHW-METER, 0, CIRCULATION-LOOP,  0, STD,  65,  80, 250, 140, 19, 3,               "Loop:",  LEFT,  -45, 5, 0, LEFT, 4, 5, "Name of the Loop this meter is attached to (Loop Type must be compatible)"
; SAC 11/30/10 - added for DOE-2.3
     COMBO, 18000,     0, 0, 1, CHW-METER, 0, LOOP-SERIES-LOCN,  0, STD,  95, 105, 275, 110, 19, 3,        "Series Locn:",  LEFT,  -75, 5, 0, LEFT, 4, 5, "For a CHW meter in series, whether at the upstream or downstream location"
   
     LABEL, "Billing Unit Thermal Value", STD, LEFT, 20, 165, 1, 0, 0, 205, 14139, 3
      EDIT, 14139, 14118, 0, 1, CHW-METER, 0,      ENERGY/UNIT,  0, STD,  80, 185,  23,  80,  0, 3,           "Btu/Unit:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Number of Btus per billing unit for this meter (e.g. 100,000 for therms)"
   
     LABEL, "Billing Units Labels", STD, LEFT, 20, 240, 1, 0, 0, 160, 14140, 3
      EDIT, 14140, 14140, 0, 1, CHW-METER, 0,       UNIT-INDEX,  0, STD,  80, 260,  23,  80,  0, 3,             "Energy:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the billing unit, used to convert english/metric units"
      EDIT, 14141, 14141, 0, 1, CHW-METER, 0,   DEM-UNIT-INDEX,  0, STD,  80, 285,  23,  80,  0, 3,             "Demand:",  LEFT,  -60, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the maximum demand billing unit"
   
     LABEL, "Equipment Capacity", STD, LEFT, 245, 60, 1, 0, 0, 425, 14142, 3
      EDIT, 14142, 14116, 0, 1, CHW-METER, 0,         CAPACITY,  0, STD, 315,  80,  23,  70,  0, 3,           "Capacity:",  LEFT,  -70, 5, 1, LEFT, 4, 5, "Capacity of the meter, defaults to product of Loop Capacity & the meter's Capacity Ratio"
      EDIT, 14143, 14117, 0, 1, CHW-METER, 0,   CAPACITY-RATIO,  0, STD, 345, 105,  23,  40,  0, 3,     "Capacity Ratio:",  LEFT, -100, 5, 1, LEFT, 4, 5, "If the meter Capacity is undefined, it is set to the product of this and the loop capacity"
   
     LABEL, "Equipment Efficiency", STD, LEFT, 470, 60, 1, 0, 0, 675, 14144, 3
      EDIT, 14144, 14119, 0, 1, CHW-METER, 0,  SOURCE-SITE-EFF,  0, STD, 585,  80,  23,  50,  3, 3, "Source-to-Site Eff:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Fraction of total energy used at the utility source that arrives at the site boundary"
   
     LABEL, "Heat Exchanger", STD, LEFT, 470, 135, 1, 0, 0, 675, 14145, 3
      EDIT, 14145, 14145, 0, 1, CHW-METER, 0,          HX-HEAD,  0, STD, 585, 155,  23,  50,  0, 3,     "Heat Exch Head:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Pressure drop through the meter's heat exchanger (if one exists)"
      EDIT, 14146, 14146, 0, 1, CHW-METER, 0,   HX-STATIC-HEAD,  0, STD, 585, 180,  23,  50,  0, 3,     "HX Static Head:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Static pressure drop through the meter's heat exchanger (zero for almost all systems)"


   ;*****************************************
   ; Direct Loads 
   ;*****************************************
   TABPAGE, 3106, 3104, 1, 3, NOTIMP, " Direct Loads "

; SAC 9/27/04 - Added access to existing INTERIOR-EU and new EXTERIOR-EU keywords
   LABEL, "Misc. Direct Loads, Interior", STD, LEFT, 25, 30, 1, 0, 0, 515, 11603, 3
     SPREAD, 11603, 11600, 0, 1, 0, PowerDOE, 0, CHWMtrInt,  0, STD,  40,  50, 120, 475, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
     
   LABEL, "Misc. Direct Loads, Exterior", STD, LEFT, 25, 195, 1, 0, 0, 515, 11602, 3
     SPREAD, 11602, 11601, 0, 1, 0, PowerDOE, 0, CHWMtrExt,  0, STD,  40, 215, 120, 475, 19, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""



 ;********************************************************************
 ;********************************************************************
 ;**
 ;**		Curve Fit Dialog
 ;**
 ;********************************************************************
 ;********************************************************************
    
; MODDLG, 2512, 2512, 1, 20, 85, 430, 560, 0, "Curve Fit", NOTIMP, 0, NOTIMP, 0
; 
;   COMBO, 12284, 12284, 0, 1, CURVE-FIT,  0,       NAME,  0, STD, 220,  10, 260, 220, 21, 3, "Currently Active Curve:",  LEFT,   80,  12, 0, LEFT, 355,  34, "Name of curve fit; options allow renaming, deleting, copying, linking, save to library"
;    LINE, 10, 40, 540, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
; 
;   COMBO, 12301, 12301, 0, 1, CURVE-FIT, 0,    NAMEOPT,  0, STD,  60,  60, 136, 250, 21, 3,          "Curve:",  LEFT,  15,  62, 0, LEFT, 205, 137, "List of all curve fits defined in project; also allows library retrieval"

MODTABDLG, 2512, 2512, 1, 100, 100, 470, 710, 0, CURVE-FIT, "Performance Curve Properties", NOTIMP, 0, NOTIMP, 0

   COMBO, 12284, 12284, 0, 1, CURVE-FIT, 0, NAME,  0, STD, 165,  15, 400, 250, 19, 3, "Currently Active Curve:",  LEFT, -150, 5, 0, LEFT, 4, 5, "List of all performance curves defined in project; also allows library retrieval and creation"
   STATIC, 1, CURVE-FIT, 0, TYPE, 0, 0, 0, 435, 20, 250, STD, LEFT, "Type: ",   "", 0, 3

    ;******************************************
    ; Curve Fit - Basic Specifications Page
    ;******************************************
    TABPAGE, 3150, 2512, 1, 3, NOTIMP, " Basic Specifications "

    EDIT, 12301, 12301, 0, 1, CURVE-FIT, 0,       NAME, -1, STD, 105,  10,  23, 250, 32, 3,     "Curve Name:",  LEFT,  -85, 5, 1, LEFT, 4, 5, "Name of performance curve; right mouse quick menu options allow deleting, copying, linking and saving to library"

   COMBO, 12244, 12244, 0, 1, CURVE-FIT, 0,       TYPE,  0, STD, 105,  65, 330, 165, 19, 3,     "Curve Type:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "The form of the Curve Fit: Linear, Bi-Linear, Quadratic, Bi-Quadratic, or Cubic"
   COMBO, 12264, 12264, 0, 1, CURVE-FIT, 0, INPUT-TYPE,  0, STD, 105,  90, 100, 165, 19, 3,     "Input Type:",  LEFT,  -85, 5, 0, LEFT, 4, 5, "Whether the curve data is Non-Dimensional, or Temperatures"
    EDIT, 12266, 12266, 0, 1, CURVE-FIT, 0, OUTPUT-MIN,  0, STD, 435,  65,  23, 110,  2, 3, "Minimum Output:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Lowest allowable value of the dependent variables; below this, this value is used"
    EDIT, 12283, 12283, 0, 1, CURVE-FIT, 0, OUTPUT-MAX,  0, STD, 435,  90,  23, 110,  2, 3, "Maximum Output:",  LEFT, -115, 5, 0, LEFT, 4, 5, "Highest allowable value of the dependent variables; above this, this value is used"
    
   LABEL, "Curve Formula:", STD, LEFT, 20, 135, 1, 0, 0, 0, 0, 3
   LABEL, "Where:",         STD, LEFT, 68, 165, 1, 0, 0, 0, 0, 3

   CASE, CURVE-FIT, 0, INPUT-TYPE, -1, =, 1, 1  ; COEFFICIENTS
      EDIT, 14828, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  0, STD, 160, 160,  23,  90,  8, 3, "a =",  LEFT,  -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
      EDIT, 14829, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  1, STD, 305, 160,  23,  90,  8, 3, "b =",  LEFT,  -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 1          ; LINEAR
         LABEL, "Z = a + bX", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
      ENDCASE
      CASE, CURVE-FIT, 0, TYPE, -1, =, 2, 2, 6       ; BI-LINEAR
         LABEL, "Z = a + bX + dY", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
         EDIT, 14830, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  3, STD, 450, 160,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
      ENDCASE
      CASE, CURVE-FIT, 0, TYPE, -1, =, 3, 3, 7, 13   ; QUADRATIC
         LABEL, "Z = a + bX + cX²", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
         EDIT, 14831, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  2, STD, 450, 160,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
      ENDCASE
      CASE, CURVE-FIT, 0, TYPE, -1, =, 2, 5, 11      ; CUBIC
         LABEL, "Z = a + bX + cX² + dX³", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
         EDIT, 14832, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  2, STD, 450, 160,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
         EDIT, 14833, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  3, STD, 160, 185,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
      ENDCASE
      CASE, ELSE                                     ; BI-QUADRATIC
         LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
         EDIT, 14834, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  2, STD, 450, 160,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
         EDIT, 14835, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  3, STD, 160, 185,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
         EDIT, 14836, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  4, STD, 305, 185,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
         EDIT, 14837, 63200, 0, 1, CURVE-FIT, 0, COEFFICIENTS,  5, STD, 450, 185,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
      ENDCASE

   ENDCASE
   CASE, ELSE   ; ENTER RAW DATA POINTS
;      LABEL, "Data Points:",   STD, LEFT, 15, 155, 1, 0, 0, 0, 0, 3

      LABEL, "Curve coefficients are calculated based on data points entered on the following tab.", STD, LEFT, 130, 215, 1, 0, 0, 0, 0, 3

      EDIT, 14838, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  0, STD, 160, 160,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
      EDIT, 14839, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  1, STD, 305, 160,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 1          ; LINEAR
;         SPREAD, 11543, 11543, 0, 1, 0,  PowerDOE, 0,   D1ThruD20, 0, SMALL,  125, 155, 109, 378, 20, 3,   "",  LEFT,   0,  0, 0, LEFT, 0, 0, ""
         LABEL, "Z = a + bX", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
      ENDCASE
      CASE, CURVE-FIT, 0, TYPE, -1, =, 2, 2, 6       ; BI-LINEAR
;         SPREAD, 11669, 11543, 0, 1, 0,  PowerDOE, 0, D1ThruD20-2, 0, SMALL,  125, 155, 109, 378, 20, 3,   "",  LEFT,   0,  0, 0, LEFT, 0, 0, ""
         LABEL, "Z = a + bX + dY", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
         EDIT, 14840, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  3, STD, 450, 160,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
      ENDCASE
      CASE, CURVE-FIT, 0, TYPE, -1, =, 3, 3, 7, 13   ; QUADRATIC
;         SPREAD, 11689, 11543, 0, 1, 0,  PowerDOE, 0,   D1ThruD20, 0, SMALL,  125, 155, 109, 378, 20, 3,   "",  LEFT,   0,  0, 0, LEFT, 0, 0, ""
         LABEL, "Z = a + bX + cX²", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
         EDIT, 14841, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  2, STD, 450, 160,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
      ENDCASE
      CASE, CURVE-FIT, 0, TYPE, -1, =, 2, 5, 11      ; CUBIC
;         SPREAD, 11690, 11543, 0, 1, 0,  PowerDOE, 0,   D1ThruD20, 0, SMALL,  125, 155, 109, 378, 20, 3,   "",  LEFT,   0,  0, 0, LEFT, 0, 0, ""
         LABEL, "Z = a + bX + cX² + dX³", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
         EDIT, 14842, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  2, STD, 450, 160,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
         EDIT, 14843, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  3, STD, 160, 185,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
      ENDCASE
      CASE, ELSE                                     ; BI-QUADRATIC
;         SPREAD, 11691, 11543, 0, 1, 0,  PowerDOE, 0, D1ThruD20-2, 0, SMALL,  125, 155, 109, 378, 20, 3,   "",  LEFT,   0,  0, 0, LEFT, 0, 0, ""
         LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 130, 135, 1, 0, 0, 0, 0, 3
         EDIT, 14844, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  2, STD, 450, 160,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
         EDIT, 14845, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  3, STD, 160, 185,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
         EDIT, 14846, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  4, STD, 305, 185,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
         EDIT, 14847, 63200, 0, 0, CURVE-FIT, 0, COEFFICIENTS,  5, STD, 450, 185,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
      ENDCASE

   ENDCASE

    ;******************************************
    ; Curve Fit - Basic Specifications Page
    ;******************************************
    TABPAGE, 3151, 2512, 1, 3, NOTIMP, " Data Points "

   CASE, CURVE-FIT, 0, INPUT-TYPE, -1, =, 1, 1  ; COEFFICIENTS
      LABEL, "Data Points are entered only for curves where Input Type = 'Raw Data Points'.", STD, LEFT, 40, 40, 1, 0, 0, 0, 0, 3
   ENDCASE
   CASE, ELSE   ; ENTER RAW DATA POINTS
      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 1   ; LINEAR
;         SPREAD, 11543, 11543, 0, 1, 0,  PowerDOE, 0,   D1ThruD20, 0, SMALL,  125, 155, 109, 378, 20, 3,   "",  LEFT,   0,  0, 0, LEFT, 0, 0, ""

        LABEL, "Data Points 1-10", STD, LEFT,   130, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Independ (X)",     STD, CENTER, 195, 40, 1, 0, 0,   0, 14852, 3
        LABEL, "Depend (Z)",       STD, CENTER, 285, 40, 1, 0, 0,   0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  0, STD, 155,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  1, STD, 155,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  2, STD, 155, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  3, STD, 155, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  4, STD, 155, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  5, STD, 155, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  6, STD, 155, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  7, STD, 155, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  8, STD, 155, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT,  9, STD, 155, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT,   370, 20, 1, 0, 0, 565, 14862, 3
        LABEL, "Independ (X)",      STD, CENTER, 435, 40, 1, 0, 0,   0, 14862, 3
        LABEL, "Depend (Z)",        STD, CENTER, 525, 40, 1, 0, 0,   0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 1,   INDEPENDENT, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 1,     DEPENDENT, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 2  ; BI-LINEAR
;         SPREAD, 11691, 11543, 0, 1, 0,  PowerDOE, 0, D1ThruD20-2, 0, SMALL,  125, 155, 109, 378, 20, 3,   "",  LEFT,   0,  0, 0, LEFT, 0, 0, ""

        LABEL, "Data Points 1-10", STD, LEFT, 40, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 105, 40, 1, 0, 0, 0, 14852, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 195, 40, 1, 0, 0, 0, 14872, 3
        LABEL, "Depend (Z)",  STD, CENTER, 285, 40, 1, 0, 0, 0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  0, STD,  65,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  1, STD,  65,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  2, STD,  65, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  3, STD,  65, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  4, STD,  65, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  5, STD,  65, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  6, STD,  65, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  7, STD,  65, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  8, STD,  65, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1,  9, STD,  65, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 10"

         EDIT, 14872, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  0, STD, 155,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 1"
         EDIT, 14873, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  1, STD, 155,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 2"
         EDIT, 14874, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  2, STD, 155, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 3"
         EDIT, 14875, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  3, STD, 155, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 4"
         EDIT, 14876, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  4, STD, 155, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 5"
         EDIT, 14877, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  5, STD, 155, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 6"
         EDIT, 14878, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  6, STD, 155, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 7"
         EDIT, 14879, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  7, STD, 155, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 8"
         EDIT, 14880, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  8, STD, 155, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 9"
         EDIT, 14881, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2,  9, STD, 155, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT, 370, 20, 1, 0, 0, 655, 14862, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 435, 40, 1, 0, 0, 0, 14862, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 525, 40, 1, 0, 0, 0, 14882, 3
        LABEL, "Depend (Z)",  STD, CENTER, 615, 40, 1, 0, 0, 0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-1, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 20"

         EDIT, 14882, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 11"
         EDIT, 14883, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 12"
         EDIT, 14884, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 13"
         EDIT, 14885, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 14"
         EDIT, 14886, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 15"
         EDIT, 14887, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 16"
         EDIT, 14888, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 17"
         EDIT, 14889, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 18"
         EDIT, 14890, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 19"
         EDIT, 14891, 63201, 0, 0, CURVE-FIT, 2, INDEPENDENT-2, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 10, STD, 575,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 11, STD, 575,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 12, STD, 575, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 13, STD, 575, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 14, STD, 575, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 15, STD, 575, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 16, STD, 575, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 17, STD, 575, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 18, STD, 575, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 2,     DEPENDENT, 19, STD, 575, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 3  ; QUADRATIC
        LABEL, "Data Points 1-10", STD, LEFT,   130, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Independ (X)",     STD, CENTER, 195, 40, 1, 0, 0,   0, 14852, 3
        LABEL, "Depend (Z)",       STD, CENTER, 285, 40, 1, 0, 0,   0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  0, STD, 155,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  1, STD, 155,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  2, STD, 155, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  3, STD, 155, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  4, STD, 155, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  5, STD, 155, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  6, STD, 155, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  7, STD, 155, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  8, STD, 155, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT,  9, STD, 155, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT,   370, 20, 1, 0, 0, 565, 14862, 3
        LABEL, "Independ (X)",      STD, CENTER, 435, 40, 1, 0, 0,   0, 14862, 3
        LABEL, "Depend (Z)",        STD, CENTER, 525, 40, 1, 0, 0,   0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 3,   INDEPENDENT, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 3,     DEPENDENT, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 4   ; BI-QUADRATIC
        LABEL, "Data Points 1-10", STD, LEFT, 40, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 105, 40, 1, 0, 0, 0, 14852, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 195, 40, 1, 0, 0, 0, 14872, 3
        LABEL, "Depend (Z)",  STD, CENTER, 285, 40, 1, 0, 0, 0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  0, STD,  65,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  1, STD,  65,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  2, STD,  65, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  3, STD,  65, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  4, STD,  65, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  5, STD,  65, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  6, STD,  65, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  7, STD,  65, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  8, STD,  65, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1,  9, STD,  65, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 10"

         EDIT, 14872, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  0, STD, 155,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 1"
         EDIT, 14873, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  1, STD, 155,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 2"
         EDIT, 14874, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  2, STD, 155, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 3"
         EDIT, 14875, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  3, STD, 155, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 4"
         EDIT, 14876, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  4, STD, 155, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 5"
         EDIT, 14877, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  5, STD, 155, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 6"
         EDIT, 14878, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  6, STD, 155, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 7"
         EDIT, 14879, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  7, STD, 155, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 8"
         EDIT, 14880, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  8, STD, 155, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 9"
         EDIT, 14881, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2,  9, STD, 155, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT, 370, 20, 1, 0, 0, 655, 14862, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 435, 40, 1, 0, 0, 0, 14862, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 525, 40, 1, 0, 0, 0, 14882, 3
        LABEL, "Depend (Z)",  STD, CENTER, 615, 40, 1, 0, 0, 0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-1, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 20"

         EDIT, 14882, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 11"
         EDIT, 14883, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 12"
         EDIT, 14884, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 13"
         EDIT, 14885, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 14"
         EDIT, 14886, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 15"
         EDIT, 14887, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 16"
         EDIT, 14888, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 17"
         EDIT, 14889, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 18"
         EDIT, 14890, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 19"
         EDIT, 14891, 63201, 0, 0, CURVE-FIT, 4, INDEPENDENT-2, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 10, STD, 575,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 11, STD, 575,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 12, STD, 575, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 13, STD, 575, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 14, STD, 575, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 15, STD, 575, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 16, STD, 575, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 17, STD, 575, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 18, STD, 575, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 4,     DEPENDENT, 19, STD, 575, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 5   ; CUBIC                
        LABEL, "Data Points 1-10", STD, LEFT,   130, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Independ (X)",     STD, CENTER, 195, 40, 1, 0, 0,   0, 14852, 3
        LABEL, "Depend (Z)",       STD, CENTER, 285, 40, 1, 0, 0,   0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  0, STD, 155,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  1, STD, 155,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  2, STD, 155, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  3, STD, 155, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  4, STD, 155, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  5, STD, 155, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  6, STD, 155, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  7, STD, 155, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  8, STD, 155, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT,  9, STD, 155, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT,   370, 20, 1, 0, 0, 565, 14862, 3
        LABEL, "Independ (X)",      STD, CENTER, 435, 40, 1, 0, 0,   0, 14862, 3
        LABEL, "Depend (Z)",        STD, CENTER, 525, 40, 1, 0, 0,   0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 5,   INDEPENDENT, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 5,     DEPENDENT, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 6   ; BI-LINEAR-T          
        LABEL, "Data Points 1-10", STD, LEFT, 40, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 105, 40, 1, 0, 0, 0, 14852, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 195, 40, 1, 0, 0, 0, 14872, 3
        LABEL, "Depend (Z)",  STD, CENTER, 285, 40, 1, 0, 0, 0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  0, STD,  65,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  1, STD,  65,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  2, STD,  65, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  3, STD,  65, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  4, STD,  65, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  5, STD,  65, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  6, STD,  65, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  7, STD,  65, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  8, STD,  65, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1,  9, STD,  65, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 10"

         EDIT, 14872, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  0, STD, 155,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 1"
         EDIT, 14873, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  1, STD, 155,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 2"
         EDIT, 14874, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  2, STD, 155, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 3"
         EDIT, 14875, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  3, STD, 155, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 4"
         EDIT, 14876, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  4, STD, 155, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 5"
         EDIT, 14877, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  5, STD, 155, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 6"
         EDIT, 14878, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  6, STD, 155, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 7"
         EDIT, 14879, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  7, STD, 155, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 8"
         EDIT, 14880, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  8, STD, 155, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 9"
         EDIT, 14881, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2,  9, STD, 155, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT, 370, 20, 1, 0, 0, 655, 14862, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 435, 40, 1, 0, 0, 0, 14862, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 525, 40, 1, 0, 0, 0, 14882, 3
        LABEL, "Depend (Z)",  STD, CENTER, 615, 40, 1, 0, 0, 0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-1, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 20"

         EDIT, 14882, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 11"
         EDIT, 14883, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 12"
         EDIT, 14884, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 13"
         EDIT, 14885, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 14"
         EDIT, 14886, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 15"
         EDIT, 14887, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 16"
         EDIT, 14888, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 17"
         EDIT, 14889, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 18"
         EDIT, 14890, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 19"
         EDIT, 14891, 63201, 0, 0, CURVE-FIT, 6, INDEPENDENT-2, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 10, STD, 575,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 11, STD, 575,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 12, STD, 575, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 13, STD, 575, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 14, STD, 575, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 15, STD, 575, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 16, STD, 575, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 17, STD, 575, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 18, STD, 575, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 6,     DEPENDENT, 19, STD, 575, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 7   ; QUADRATIC-T          
        LABEL, "Data Points 1-10", STD, LEFT,   130, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Independ (X)",     STD, CENTER, 195, 40, 1, 0, 0,   0, 14852, 3
        LABEL, "Depend (Z)",       STD, CENTER, 285, 40, 1, 0, 0,   0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  0, STD, 155,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  1, STD, 155,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  2, STD, 155, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  3, STD, 155, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  4, STD, 155, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  5, STD, 155, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  6, STD, 155, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  7, STD, 155, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  8, STD, 155, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT,  9, STD, 155, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT,   370, 20, 1, 0, 0, 565, 14862, 3
        LABEL, "Independ (X)",      STD, CENTER, 435, 40, 1, 0, 0,   0, 14862, 3
        LABEL, "Depend (Z)",        STD, CENTER, 525, 40, 1, 0, 0,   0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 7,   INDEPENDENT, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 7,     DEPENDENT, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 8   ; BI-QUADRATIC-T       
        LABEL, "Data Points 1-10", STD, LEFT, 40, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 105, 40, 1, 0, 0, 0, 14852, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 195, 40, 1, 0, 0, 0, 14872, 3
        LABEL, "Depend (Z)",  STD, CENTER, 285, 40, 1, 0, 0, 0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  0, STD,  65,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  1, STD,  65,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  2, STD,  65, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  3, STD,  65, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  4, STD,  65, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  5, STD,  65, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  6, STD,  65, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  7, STD,  65, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  8, STD,  65, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1,  9, STD,  65, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 10"

         EDIT, 14872, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  0, STD, 155,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 1"
         EDIT, 14873, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  1, STD, 155,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 2"
         EDIT, 14874, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  2, STD, 155, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 3"
         EDIT, 14875, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  3, STD, 155, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 4"
         EDIT, 14876, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  4, STD, 155, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 5"
         EDIT, 14877, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  5, STD, 155, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 6"
         EDIT, 14878, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  6, STD, 155, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 7"
         EDIT, 14879, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  7, STD, 155, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 8"
         EDIT, 14880, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  8, STD, 155, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 9"
         EDIT, 14881, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2,  9, STD, 155, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT, 370, 20, 1, 0, 0, 655, 14862, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 435, 40, 1, 0, 0, 0, 14862, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 525, 40, 1, 0, 0, 0, 14882, 3
        LABEL, "Depend (Z)",  STD, CENTER, 615, 40, 1, 0, 0, 0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-1, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 20"

         EDIT, 14882, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 11"
         EDIT, 14883, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 12"
         EDIT, 14884, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 13"
         EDIT, 14885, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 14"
         EDIT, 14886, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 15"
         EDIT, 14887, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 16"
         EDIT, 14888, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 17"
         EDIT, 14889, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 18"
         EDIT, 14890, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 19"
         EDIT, 14891, 63201, 0, 0, CURVE-FIT, 8, INDEPENDENT-2, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 10, STD, 575,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 11, STD, 575,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 12, STD, 575, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 13, STD, 575, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 14, STD, 575, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 15, STD, 575, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 16, STD, 575, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 17, STD, 575, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 18, STD, 575, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 8,     DEPENDENT, 19, STD, 575, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 9   ; BI-QUADRATIC-DT&T    
        LABEL, "Data Points 1-10", STD, LEFT, 40, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 105, 40, 1, 0, 0, 0, 14852, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 195, 40, 1, 0, 0, 0, 14872, 3
        LABEL, "Depend (Z)",  STD, CENTER, 285, 40, 1, 0, 0, 0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  0, STD,  65,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  1, STD,  65,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  2, STD,  65, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  3, STD,  65, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  4, STD,  65, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  5, STD,  65, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  6, STD,  65, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  7, STD,  65, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  8, STD,  65, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1,  9, STD,  65, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 10"

         EDIT, 14872, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  0, STD, 155,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 1"
         EDIT, 14873, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  1, STD, 155,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 2"
         EDIT, 14874, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  2, STD, 155, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 3"
         EDIT, 14875, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  3, STD, 155, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 4"
         EDIT, 14876, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  4, STD, 155, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 5"
         EDIT, 14877, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  5, STD, 155, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 6"
         EDIT, 14878, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  6, STD, 155, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 7"
         EDIT, 14879, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  7, STD, 155, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 8"
         EDIT, 14880, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  8, STD, 155, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 9"
         EDIT, 14881, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2,  9, STD, 155, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT, 370, 20, 1, 0, 0, 655, 14862, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 435, 40, 1, 0, 0, 0, 14862, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 525, 40, 1, 0, 0, 0, 14882, 3
        LABEL, "Depend (Z)",  STD, CENTER, 615, 40, 1, 0, 0, 0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-1, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 20"

         EDIT, 14882, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 11"
         EDIT, 14883, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 12"
         EDIT, 14884, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 13"
         EDIT, 14885, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 14"
         EDIT, 14886, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 15"
         EDIT, 14887, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 16"
         EDIT, 14888, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 17"
         EDIT, 14889, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 18"
         EDIT, 14890, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 19"
         EDIT, 14891, 63201, 0, 0, CURVE-FIT, 9, INDEPENDENT-2, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 10, STD, 575,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 11, STD, 575,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 12, STD, 575, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 13, STD, 575, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 14, STD, 575, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 15, STD, 575, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 16, STD, 575, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 17, STD, 575, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 18, STD, 575, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 9,     DEPENDENT, 19, STD, 575, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 10  ; BI-QUADRATIC-RATIO&T 
        LABEL, "Data Points 1-10", STD, LEFT, 40, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 105, 40, 1, 0, 0, 0, 14852, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 195, 40, 1, 0, 0, 0, 14872, 3
        LABEL, "Depend (Z)",  STD, CENTER, 285, 40, 1, 0, 0, 0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  0, STD,  65,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  1, STD,  65,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  2, STD,  65, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  3, STD,  65, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  4, STD,  65, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  5, STD,  65, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  6, STD,  65, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  7, STD,  65, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  8, STD,  65, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1,  9, STD,  65, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 10"

         EDIT, 14872, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  0, STD, 155,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 1"
         EDIT, 14873, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  1, STD, 155,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 2"
         EDIT, 14874, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  2, STD, 155, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 3"
         EDIT, 14875, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  3, STD, 155, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 4"
         EDIT, 14876, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  4, STD, 155, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 5"
         EDIT, 14877, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  5, STD, 155, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 6"
         EDIT, 14878, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  6, STD, 155, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 7"
         EDIT, 14879, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  7, STD, 155, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 8"
         EDIT, 14880, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  8, STD, 155, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 9"
         EDIT, 14881, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2,  9, STD, 155, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT, 370, 20, 1, 0, 0, 655, 14862, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 435, 40, 1, 0, 0, 0, 14862, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 525, 40, 1, 0, 0, 0, 14882, 3
        LABEL, "Depend (Z)",  STD, CENTER, 615, 40, 1, 0, 0, 0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-1, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 20"

         EDIT, 14882, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 11"
         EDIT, 14883, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 12"
         EDIT, 14884, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 13"
         EDIT, 14885, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 14"
         EDIT, 14886, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 15"
         EDIT, 14887, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 16"
         EDIT, 14888, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 17"
         EDIT, 14889, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 18"
         EDIT, 14890, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 19"
         EDIT, 14891, 63201, 0, 0, CURVE-FIT, 10, INDEPENDENT-2, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 10, STD, 575,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 11, STD, 575,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 12, STD, 575, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 13, STD, 575, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 14, STD, 575, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 15, STD, 575, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 16, STD, 575, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 17, STD, 575, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 18, STD, 575, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 10,     DEPENDENT, 19, STD, 575, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 11  ; CUBIC-T              
        LABEL, "Data Points 1-10", STD, LEFT,   130, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Independ (X)",     STD, CENTER, 195, 40, 1, 0, 0,   0, 14852, 3
        LABEL, "Depend (Z)",       STD, CENTER, 285, 40, 1, 0, 0,   0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  0, STD, 155,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  1, STD, 155,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  2, STD, 155, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  3, STD, 155, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  4, STD, 155, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  5, STD, 155, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  6, STD, 155, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  7, STD, 155, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  8, STD, 155, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT,  9, STD, 155, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT,   370, 20, 1, 0, 0, 565, 14862, 3
        LABEL, "Independ (X)",      STD, CENTER, 435, 40, 1, 0, 0,   0, 14862, 3
        LABEL, "Depend (Z)",        STD, CENTER, 525, 40, 1, 0, 0,   0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 11,   INDEPENDENT, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 11,     DEPENDENT, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 12  ; BI-QUADRATIC-T&RATIO 
        LABEL, "Data Points 1-10", STD, LEFT, 40, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 105, 40, 1, 0, 0, 0, 14852, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 195, 40, 1, 0, 0, 0, 14872, 3
        LABEL, "Depend (Z)",  STD, CENTER, 285, 40, 1, 0, 0, 0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  0, STD,  65,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  1, STD,  65,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  2, STD,  65, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  3, STD,  65, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  4, STD,  65, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  5, STD,  65, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  6, STD,  65, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  7, STD,  65, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  8, STD,  65, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1,  9, STD,  65, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 10"

         EDIT, 14872, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  0, STD, 155,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 1"
         EDIT, 14873, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  1, STD, 155,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 2"
         EDIT, 14874, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  2, STD, 155, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 3"
         EDIT, 14875, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  3, STD, 155, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 4"
         EDIT, 14876, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  4, STD, 155, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 5"
         EDIT, 14877, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  5, STD, 155, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 6"
         EDIT, 14878, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  6, STD, 155, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 7"
         EDIT, 14879, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  7, STD, 155, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 8"
         EDIT, 14880, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  8, STD, 155, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 9"
         EDIT, 14881, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2,  9, STD, 155, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT, 370, 20, 1, 0, 0, 655, 14862, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 435, 40, 1, 0, 0, 0, 14862, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 525, 40, 1, 0, 0, 0, 14882, 3
        LABEL, "Depend (Z)",  STD, CENTER, 615, 40, 1, 0, 0, 0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-1, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 20"

         EDIT, 14882, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 11"
         EDIT, 14883, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 12"
         EDIT, 14884, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 13"
         EDIT, 14885, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 14"
         EDIT, 14886, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 15"
         EDIT, 14887, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 16"
         EDIT, 14888, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 17"
         EDIT, 14889, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 18"
         EDIT, 14890, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 19"
         EDIT, 14891, 63201, 0, 0, CURVE-FIT, 12, INDEPENDENT-2, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 10, STD, 575,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 11, STD, 575,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 12, STD, 575, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 13, STD, 575, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 14, STD, 575, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 15, STD, 575, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 16, STD, 575, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 17, STD, 575, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 18, STD, 575, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 12,     DEPENDENT, 19, STD, 575, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 13  ; QUADRATIC-DT         
        LABEL, "Data Points 1-10", STD, LEFT,   130, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Independ (X)",     STD, CENTER, 195, 40, 1, 0, 0,   0, 14852, 3
        LABEL, "Depend (Z)",       STD, CENTER, 285, 40, 1, 0, 0,   0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  0, STD, 155,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  1, STD, 155,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  2, STD, 155, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  3, STD, 155, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  4, STD, 155, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  5, STD, 155, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  6, STD, 155, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  7, STD, 155, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  8, STD, 155, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT,  9, STD, 155, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT,   370, 20, 1, 0, 0, 565, 14862, 3
        LABEL, "Independ (X)",      STD, CENTER, 435, 40, 1, 0, 0,   0, 14862, 3
        LABEL, "Depend (Z)",        STD, CENTER, 525, 40, 1, 0, 0,   0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 13,   INDEPENDENT, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent data point (X) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 13,     DEPENDENT, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, CURVE-FIT, 0, TYPE, -1, =, 1, 14  ; BI-QUADRATIC-RATIO&DT
        LABEL, "Data Points 1-10", STD, LEFT, 40, 20, 1, 0, 0, 325, 14852, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 105, 40, 1, 0, 0, 0, 14852, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 195, 40, 1, 0, 0, 0, 14872, 3
        LABEL, "Depend (Z)",  STD, CENTER, 285, 40, 1, 0, 0, 0, 14892, 3

         EDIT, 14852, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  0, STD,  65,  60,  23,  80,  3, 3,  "1:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 1"
         EDIT, 14853, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  1, STD,  65,  85,  23,  80,  3, 3,  "2:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 2"
         EDIT, 14854, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  2, STD,  65, 110,  23,  80,  3, 3,  "3:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 3"
         EDIT, 14855, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  3, STD,  65, 135,  23,  80,  3, 3,  "4:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 4"
         EDIT, 14856, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  4, STD,  65, 160,  23,  80,  3, 3,  "5:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 5"
         EDIT, 14857, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  5, STD,  65, 185,  23,  80,  3, 3,  "6:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 6"
         EDIT, 14858, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  6, STD,  65, 210,  23,  80,  3, 3,  "7:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 7"
         EDIT, 14859, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  7, STD,  65, 235,  23,  80,  3, 3,  "8:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 8"
         EDIT, 14860, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  8, STD,  65, 260,  23,  80,  3, 3,  "9:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 9"
         EDIT, 14861, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1,  9, STD,  65, 285,  23,  80,  3, 3, "10:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 10"

         EDIT, 14872, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  0, STD, 155,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 1"
         EDIT, 14873, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  1, STD, 155,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 2"
         EDIT, 14874, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  2, STD, 155, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 3"
         EDIT, 14875, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  3, STD, 155, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 4"
         EDIT, 14876, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  4, STD, 155, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 5"
         EDIT, 14877, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  5, STD, 155, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 6"
         EDIT, 14878, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  6, STD, 155, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 7"
         EDIT, 14879, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  7, STD, 155, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 8"
         EDIT, 14880, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  8, STD, 155, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 9"
         EDIT, 14881, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2,  9, STD, 155, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 10"

         EDIT, 14892, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  0, STD, 245,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 1"
         EDIT, 14893, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  1, STD, 245,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 2"
         EDIT, 14894, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  2, STD, 245, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 3"
         EDIT, 14895, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  3, STD, 245, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 4"
         EDIT, 14896, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  4, STD, 245, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 5"
         EDIT, 14897, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  5, STD, 245, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 6"
         EDIT, 14898, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  6, STD, 245, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 7"
         EDIT, 14899, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  7, STD, 245, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 8"
         EDIT, 14900, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  8, STD, 245, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 9"
         EDIT, 14901, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT,  9, STD, 245, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 10"

        LABEL, "Data Points 11-20", STD, LEFT, 370, 20, 1, 0, 0, 655, 14862, 3
        LABEL, "Indep-1 (X)", STD, CENTER, 435, 40, 1, 0, 0, 0, 14862, 3
        LABEL, "Indep-2 (Y)", STD, CENTER, 525, 40, 1, 0, 0, 0, 14882, 3
        LABEL, "Depend (Z)",  STD, CENTER, 615, 40, 1, 0, 0, 0, 14902, 3

         EDIT, 14862, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 10, STD, 395,  60,  23,  80,  3, 3, "11:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 11"
         EDIT, 14863, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 11, STD, 395,  85,  23,  80,  3, 3, "12:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 12"
         EDIT, 14864, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 12, STD, 395, 110,  23,  80,  3, 3, "13:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 13"
         EDIT, 14865, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 13, STD, 395, 135,  23,  80,  3, 3, "14:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 14"
         EDIT, 14866, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 14, STD, 395, 160,  23,  80,  3, 3, "15:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 15"
         EDIT, 14867, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 15, STD, 395, 185,  23,  80,  3, 3, "16:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 16"
         EDIT, 14868, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 16, STD, 395, 210,  23,  80,  3, 3, "17:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 17"
         EDIT, 14869, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 17, STD, 395, 235,  23,  80,  3, 3, "18:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 18"
         EDIT, 14870, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 18, STD, 395, 260,  23,  80,  3, 3, "19:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 19"
         EDIT, 14871, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-1, 19, STD, 395, 285,  23,  80,  3, 3, "20:",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-1 data point (X) # 20"

         EDIT, 14882, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 10, STD, 485,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 11"
         EDIT, 14883, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 11, STD, 485,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 12"
         EDIT, 14884, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 12, STD, 485, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 13"
         EDIT, 14885, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 13, STD, 485, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 14"
         EDIT, 14886, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 14, STD, 485, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 15"
         EDIT, 14887, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 15, STD, 485, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 16"
         EDIT, 14888, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 16, STD, 485, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 17"
         EDIT, 14889, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 17, STD, 485, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 18"
         EDIT, 14890, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 18, STD, 485, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 19"
         EDIT, 14891, 63201, 0, 0, CURVE-FIT, 14, INDEPENDENT-2, 19, STD, 485, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Independent-2 data point (Y) # 20"

         EDIT, 14902, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 10, STD, 575,  60,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 11"
         EDIT, 14903, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 11, STD, 575,  85,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 12"
         EDIT, 14904, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 12, STD, 575, 110,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 13"
         EDIT, 14905, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 13, STD, 575, 135,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 14"
         EDIT, 14906, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 14, STD, 575, 160,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 15"
         EDIT, 14907, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 15, STD, 575, 185,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 16"
         EDIT, 14908, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 16, STD, 575, 210,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 17"
         EDIT, 14909, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 17, STD, 575, 235,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 18"
         EDIT, 14910, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 18, STD, 575, 260,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 19"
         EDIT, 14911, 63201, 0, 0, CURVE-FIT, 14,     DEPENDENT, 19, STD, 575, 285,  23,  80,  3, 3,    "",  LEFT, -25, 5, 0, LEFT, 4, 5, "Dependent data point (Z) # 20"
      ENDCASE

      CASE, ELSE 
      LABEL, "Unrecognized curve type.", STD, LEFT, 40, 40, 1, 0, 0, 0, 0, 3
      ENDCASE
   ENDCASE


 ;********************************************************************
 ;********************************************************************
 ;**
 ;**		Performance Data Dialog
 ;**
 ;********************************************************************
 ;********************************************************************
    

MODTABDLG, 3371, 0, 1, 100, 100, 660, 710, 0, PERFORMANCE-DATA, "Equipment Performance Data", NOTIMP, 0, NOTIMP, 0

   COMBO, 18320, 0, 0, 1, PERFORMANCE-DATA, 0, NAME,  0, STD, 165,  15, 400, 250, 19, 3, "Currently Active Curve:",  LEFT, -150, 5, 0, LEFT, 4, 5, "List of all performance curves defined in project; also allows library retrieval and creation"
   STATIC, 1, PERFORMANCE-DATA, 0, TYPE, 0, 0, 0, 435, 20, 250, STD, LEFT, "Type: ",   "", 0, 3

    ;**********************************************
    ; Performance Data - Basic Specifications Tab
    ;**********************************************
    TABPAGE, 3372, 2512, 1, 3, NOTIMP, " Basic Specifications "

   EDIT, 18384, 0, 0, 1, PERFORMANCE-DATA, 0, C-MANUFACTURER, -1, STD, 140,   5,  23, 460, 76, 3, "Manufacturer(s):", LEFT, -115, 5, 1, LEFT, 4, 5, "The manufacturer of the equipment"
   EDIT, 18385, 0, 0, 1, PERFORMANCE-DATA, 0, C-MODEL-NUMBER, -1, STD, 140,  30,  23, 460, 76, 3, "Model Number(s):", LEFT, -115, 5, 1, LEFT, 4, 5, "The model number of the equipment"
   COMBO,18386, 0, 0, 1, PERFORMANCE-DATA, 0, COMP-OPTION,     0, STD, 140,  55, 250, 140, 19, 3, "Code Compliance:", LEFT, -115, 5, 0, LEFT, 4, 5, ""
 

   CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 2, 1, 2  ; DX-COOLING and DX-HEATPUMP

      LABEL, "DX Unit Design Parameters", STD, LEFT, 25,  85, 0, 0, 1, 625, 0, 3
      
      EDIT, 18961, 0, 0, 1, PERFORMANCE-DATA, 0, NET-CLG-CAPACITY,-1, STD, 140, 130,  23, 140,  3, 3,"ARI Cool Capacity:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 18962, 0, 0, 1, PERFORMANCE-DATA, 0, GRS-CLG-CAPACITY,-1, STD, 140, 155,  23, 140,  3, 3,"Gross Cool Cap:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 18963, 0, 0, 1, PERFORMANCE-DATA, 0, COOLING-EER     ,-1, STD, 140, 180,  23, 140,  3, 3,"ARI Rated EER:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      
      EDIT, 18964, 0, 0, 1, PERFORMANCE-DATA, 0, MIN-UNLOAD-RATIO,-1, STD, 460, 130,  23, 140,  3, 3,"Min Unload Ratio:",  LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 18965, 0, 0, 1, PERFORMANCE-DATA, 0, MIN-HGB-RATIO   ,-1, STD, 460, 155,  23, 140,  3, 3,"Min HGB Ratio:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      
      CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 1, 2     ; heatpump
      
      EDIT, 18966, 0, 0, 1, PERFORMANCE-DATA, 0, NET-HTG-CAPACITY,-1, STD, 140, 230,  23, 140,  3, 3,"ARI Heat Capacity:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 18967, 0, 0, 1, PERFORMANCE-DATA, 0, GRS-HTG-CAPACITY,-1, STD, 140, 255,  23, 140,  3, 3,"Gross Heat Cap:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 18968, 0, 0, 1, PERFORMANCE-DATA, 0, HEATING-COP     ,-1, STD, 140, 280,  23, 140,  3, 3,"ARI Rated COP:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      ENDCASE

   ENDCASE
   CASE, ELSE   ; CHILLER-AIR-COOLED and CHILLER-WATER-COOLED

      LABEL, "Chiller Design Parameters", STD, LEFT, 25,  85, 0, 0, 1, 625, 0, 3
      COMBO,18387, 0, 0, 1, PERFORMANCE-DATA, 0, VARIABLE-SPEED,   0, STD, 140, 105, 250, 140, 19, 3, "Variable Speed:", LEFT, -115, 5, 0, LEFT, 4, 5, ""
      EDIT, 18388, 0, 0, 1, PERFORMANCE-DATA, 0, DESIGN-CHW-T,    -1, STD, 140, 130,  23, 140,  3, 3,  "Leaving CHW T:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 18389, 0, 0, 1, PERFORMANCE-DATA, 0, DESIGN-CHW-FLOW, -1, STD, 140, 155,  23, 140,  3, 3,"Evaporator Flow:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
 
 

      CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 1, 3     ; water-cooled chillers
   
      EDIT, 18391, 0, 0, 1, PERFORMANCE-DATA, 0, DESIGN-COND-T,   -1, STD, 460, 130,  23, 140,  3, 3, "Entering CW T:",  LEFT, -115, 5, 1, LEFT, 4, 5, ""
      EDIT, 18390, 0, 0, 1, PERFORMANCE-DATA, 0, DESIGN-CW-DP,    -1, STD, 460, 155,  23, 140,  3, 3,"Evaporator Head:", LEFT, -115, 5, 1, LEFT, 4, 5, ""
    
      ENDCASE
      CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 1, 4     ; air-cooled chillers
      ENDCASE

     LABEL, "Chiller Performance Metrics", STD, LEFT, 25, 190, 0, 0, 1, 625, 0, 3
     LABEL, "IPLV/NPLV Data",          BOLD,  CENTER,  300, 210, 1, 0, 0,   0, 0, 3
     LABEL, "ChW T"    ,                STD,  CENTER,  150, 230, 1, 0, 0,   0, 0, 3
     LABEL, "CW T"     ,                STD,  CENTER,  250, 230, 1, 0, 0,   0, 0, 3
     LABEL, "Capacity" ,                STD,  CENTER,  350, 230, 1, 0, 0,   0, 0, 3
     LABEL, "Power"    ,                STD,  CENTER,  450, 230, 1, 0, 0,   0, 0, 3

     EDIT, 18931, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-CHWT     ,    0, STD, 100, 250,  23,  95,  2, 3,  "100%:",  LEFT,  -40, 0, 0, LEFT, 4, 5, ""
     EDIT, 18932, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-COND-T   ,    0, STD, 200, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18933, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-CLG-CAP  ,    0, STD, 300, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18934, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-POWER    ,    0, STD, 400, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18935, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-CHWT     ,    1, STD, 100, 275,  23,  95,  2, 3,  " 75%:",  LEFT,  -40, 0, 0, LEFT, 4, 5, ""
     EDIT, 18936, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-COND-T   ,    1, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18937, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-CLG-CAP  ,    1, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18938, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-POWER    ,    1, STD, 400, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18939, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-CHWT     ,    2, STD, 100, 300,  23,  95,  2, 3,  " 50%:",  LEFT,  -40, 0, 0, LEFT, 4, 5, ""
     EDIT, 18940, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-COND-T   ,    2, STD, 200, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18941, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-CLG-CAP  ,    2, STD, 300, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18942, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-POWER    ,    2, STD, 400, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18943, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-CHWT     ,    3, STD, 100, 325,  23,  95,  2, 3,  " 25%:",  LEFT,  -40, 0, 0, LEFT, 4, 5, ""
     EDIT, 18944, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-COND-T   ,    3, STD, 200, 325,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18945, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-CLG-CAP  ,    3, STD, 300, 325,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18946, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-POWER    ,    3, STD, 400, 325,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     LABEL, "Calculated kW/Ton",       BOLD,  CENTER,  250, 380, 1, 0, 0,   0, 0, 3
     LABEL, "From Data",                STD,  CENTER,  150, 400, 1, 0, 0,   0, 0, 3
     LABEL, "From Curve",               STD,  CENTER,  250, 400, 1, 0, 0,   0, 0, 3
     LABEL, "% Error"  ,                STD,  CENTER,  350, 400, 1, 0, 0,   0, 0, 3

     EDIT, 18951, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-DATA  ,     0, STD, 100, 425,  23,  95,  2, 3,  "100%:",  LEFT,  -40, 0, 0, LEFT, 4, 5, ""
     EDIT, 18952, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-CURVE ,     0, STD, 200, 425,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18953, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-PCT-ERROR,  0, STD, 300, 425,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18955, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-DATA  ,     1, STD, 100, 450,  23,  95,  2, 3,  " 75%:",  LEFT,  -40, 0, 0, LEFT, 4, 5, ""
     EDIT, 18956, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-CURVE ,     1, STD, 200, 450,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18957, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-PCT-ERROR,  1, STD, 300, 450,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18959, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-DATA  ,     2, STD, 100, 475,  23,  95,  2, 3,  " 50%:",  LEFT,  -40, 0, 0, LEFT, 4, 5, ""
     EDIT, 18960, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-CURVE ,     2, STD, 200, 475,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18961, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-PCT-ERROR,  2, STD, 300, 475,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18963, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-DATA  ,     3, STD, 100, 500,  23,  95,  2, 3,  " 25%:",  LEFT,  -40, 0, 0, LEFT, 4, 5, ""
     EDIT, 18964, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-CURVE ,     3, STD, 200, 500,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18965, 0, 0, 0, PERFORMANCE-DATA, 3,   KW/TON-PCT-ERROR,  3, STD, 300, 500,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18963, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-DATA    ,     0, STD, 100, 525,  23,  95,  2, 3,  "IPLV/NPLV:",  LEFT,  -70, 0, 0, LEFT, 4, 5, ""
     EDIT, 18964, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-CURVE   ,     0, STD, 200, 525,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18965, 0, 0, 0, PERFORMANCE-DATA, 3,   IPLV-PCT-ERROR  ,  0, STD, 300, 525,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
   ENDCASE

    ;******************************************
    ; Performance Data - Cool Capacity Tab
    ;******************************************
    TABPAGE, 3373, 0, 1, 3, NOTIMP, " CoolCapf(t) "

   CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 2, 3, 4  ; water and air cooled chillers

     CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 1, 3  ; water cooled chillers
       LABEL, "Water Chilling Capacity = f(ChwT,CWT) - User Data",   BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
       LABEL, "Entering Condenser Water Temperature",                STD,  LEFT,  250, 28, 1, 0, 0,   0, 0, 3
       LABEL, "Water Chilling Capacity = f(ChwT,CWT) - Normalized",  BOLD, LEFT,   15, 240, 1, 0, 0, 400, 0, 3
       LABEL, "Entering Condenser Water Temperature",                STD,  LEFT,  250, 258, 1, 0, 0,   0, 0, 3
     ENDCASE
     CASE, ELSE
       LABEL, "Water Chilling Capacity = f(ChwT,ODB) - User Data", BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
       LABEL, "Entering Condenser Air Temperature",                STD,  LEFT,  250, 28, 1, 0, 0,   0, 0, 3
       LABEL, "Water Chilling Capacity = f(ChwT,ODB) - Normalized",BOLD, LEFT,   15, 240, 1, 0, 0, 400, 0, 3
       LABEL, "Entering Condenser Air Temperature",                STD,  LEFT,  250, 258, 1, 0, 0,   0, 0, 3
     ENDCASE
     LABEL, "Leaving",                                   STD,  LEFT,   25, 41, 1, 0, 0,   0, 0, 3
     LABEL, "ChW T  ",                                   STD,  LEFT,   25, 55, 1, 0, 0,   0, 0, 3
      LINE,  20, 70, 600,  70, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 40,  95, 180, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18581, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      0, STD, 100,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18582, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      1, STD, 200,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18583, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      2, STD, 300,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18584, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      3, STD, 400,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18585, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      4, STD, 500,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18586, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT1,        0, STD,  20,  75,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18587, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     0, STD, 100,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18588, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     1, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18589, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     2, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18590, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     3, STD, 400,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18591, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     4, STD, 500,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18592, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT1,        1, STD,  20, 100,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18593, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     5, STD, 100, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18594, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     6, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18595, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     7, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18596, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     8, STD, 400, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18597, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,     9, STD, 500, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18598, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT1,        2, STD,  20, 125,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18599, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    10, STD, 100, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18600, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    11, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18601, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    12, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18602, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    13, STD, 400, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18603, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    14, STD, 500, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18604, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT1,        3, STD,  20, 150,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18605, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    15, STD, 100, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18606, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    16, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18607, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    17, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18608, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    18, STD, 400, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18609, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-TEMP,    19, STD, 500, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "Leaving",                                     STD,  LEFT,   25, 271, 1, 0, 0,   0, 0, 3
     LABEL, "ChW T  ",                                     STD,  LEFT,   25, 285, 1, 0, 0,   0, 0, 3
      LINE,  20, 300, 600, 300, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 270,  95, 410, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18610, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      0, STD, 100, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18611, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      1, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18612, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      2, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18613, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      3, STD, 400, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18614, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T1,      4, STD, 500, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18615, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT1,        0, STD,  20, 305,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18616, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    0, STD, 100, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18617, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    1, STD, 200, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18618, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    2, STD, 300, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18619, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    3, STD, 400, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18620, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    4, STD, 500, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18621, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT1,        1, STD,  20, 330,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18622, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    5, STD, 100, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18623, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    6, STD, 200, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18624, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    7, STD, 300, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18625, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    8, STD, 400, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18626, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,    9, STD, 500, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18627, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT1,        2, STD,  20, 355,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18628, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   10, STD, 100, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18629, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   11, STD, 200, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18630, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   12, STD, 300, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18631, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   13, STD, 400, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18632, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   14, STD, 500, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18633, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT1,        3, STD,  20, 380,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18634, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   15, STD, 100, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18635, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   16, STD, 200, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18636, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   17, STD, 300, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18637, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   18, STD, 400, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18638, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CAP-NTEMP,   19, STD, 500, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""


     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18639, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18640, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18641, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18642, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18643, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18644, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
     

   ENDCASE

   CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 2, 1, 2  ; DX cooling and heatpump
   
     LABEL, "Cooling Capacity = f(EWB,ODB) - User Data", BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
     LABEL, "Entering Wetbulb Temperature",              STD,  LEFT,  150, 28, 1, 0, 0,   0, 0, 3
     LABEL, "Outdoor",                                   STD,  LEFT,   25, 41, 1, 0, 0,   0, 0, 3
     LABEL, "DB Temp",                                   STD,  LEFT,   25, 55, 1, 0, 0,   0, 0, 3
      LINE,  20, 70, 400,  70, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 40,  95, 225, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18391, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB1,       0, STD, 100,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18392, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB1,       1, STD, 200,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18393, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB1,       2, STD, 300,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18394, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       0, STD,  20,  75,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18395, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   0, STD, 100,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18396, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   1, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18397, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   2, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18398, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       1, STD,  20, 100,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18399, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   3, STD, 100, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18400, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   4, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18401, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   5, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18402, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       2, STD,  20, 125,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18403, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   6, STD, 100, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18404, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   7, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18405, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   8, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18406, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       3, STD,  20, 150,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18407, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,   9, STD, 100, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18408, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,  10, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18409, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,  11, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18410, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       4, STD,  20, 175,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18411, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,  12, STD, 100, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18412, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,  13, STD, 200, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18413, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,  14, STD, 300, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18414, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       5, STD,  20, 200,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18415, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,  15, STD, 100, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18416, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,  16, STD, 200, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18417, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-TEMP,  17, STD, 300, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "Cooling Capacity = f(EWB,ODB) - Normalized",  BOLD, LEFT,   15, 240, 1, 0, 0, 400, 0, 3
     LABEL, "Entering Wetbulb Temperature",                STD,  LEFT,  150, 258, 1, 0, 0,   0, 0, 3
     LABEL, "Outdoor",                                     STD,  LEFT,   25, 271, 1, 0, 0,   0, 0, 3
     LABEL, "DB Temp",                                     STD,  LEFT,   25, 285, 1, 0, 0,   0, 0, 3
      LINE,  20, 300, 400, 300, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 270,  95, 455, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18418, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB1,       0, STD, 100, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18419, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB1,       1, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18420, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB1,       2, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18421, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       0, STD,  20, 305,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18422, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  0, STD, 100, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18423, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  1, STD, 200, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18424, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  2, STD, 300, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18425, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       1, STD,  20, 330,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18426, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  3, STD, 100, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18427, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  4, STD, 200, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18428, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  5, STD, 300, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18429, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       2, STD,  20, 355,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18430, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  6, STD, 100, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18421, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  7, STD, 200, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18422, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  8, STD, 300, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18423, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       3, STD,  20, 380,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18424, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP,  9, STD, 100, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18425, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP, 10, STD, 200, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18426, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP, 11, STD, 300, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18427, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       4, STD,  20, 405,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18428, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP, 12, STD, 100, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18429, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP, 13, STD, 200, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18430, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP, 14, STD, 300, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18431, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB1,       5, STD,  20, 430,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18432, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP, 15, STD, 100, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18433, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP, 16, STD, 200, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18434, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-NTEMP, 17, STD, 300, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18435, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18436, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18437, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18438, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18439, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18440, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
     
   ENDCASE

    ;******************************************
    ; Performance Data - Cool EIR Tab
    ;******************************************
    TABPAGE, 3374, 0, 1, 3, NOTIMP, " CoolEIRf(t) "

   CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 2, 3, 4  ; water and air cooled chillers

     CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 1, 3  ; water cooled chillers
       LABEL, "Water Chiller Power = f(ChwT,CWT) - User Data",    BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
       LABEL, "Entering",                                     STD,  LEFT,   25, 41, 1, 0, 0,   0, 0, 3
       LABEL, "Cond Wtr",                                     STD,  LEFT,   25, 55, 1, 0, 0,   0, 0, 3
       LABEL, "Water Chiller Power = f(ChwT,CWT) - Normalized",   BOLD, LEFT,   15, 240, 1, 0, 0, 400, 0, 3
       LABEL, "Entering",                                     STD,  LEFT,   25, 271, 1, 0, 0,   0, 0, 3
       LABEL, "Cond Wtr",                                     STD,  LEFT,   25, 285, 1, 0, 0,   0, 0, 3
     ENDCASE
     CASE, ELSE
       LABEL, "Water Chiller Power = f(ChWT,ODB) - User Data",    BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
       LABEL, "Entering",                                     STD,  LEFT,   25, 41, 1, 0, 0,   0, 0, 3
       LABEL, "Cond Air",                                     STD,  LEFT,   25, 55, 1, 0, 0,   0, 0, 3
       LABEL, "Water Chiller Power = f(ChWT,ODB) - Normalized",   BOLD, LEFT,   15, 240, 1, 0, 0, 400, 0, 3
       LABEL, "Entering",                                     STD,  LEFT,   25, 271, 1, 0, 0,   0, 0, 3
       LABEL, "Cond Air",                                     STD,  LEFT,   25, 285, 1, 0, 0,   0, 0, 3
     ENDCASE
     LABEL, "Leaving Chilled Water Temperature",                STD,  LEFT,  250, 28, 1, 0, 0,   0, 0, 3
      LINE,  20, 70, 600,  70, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 40,  95, 180, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18641, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      0, STD, 100,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18642, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      1, STD, 200,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18643, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      2, STD, 300,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18644, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      3, STD, 400,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18645, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      4, STD, 500,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18646, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT2,        0, STD,  20,  75,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18647, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     0, STD, 100,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18648, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     1, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18649, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     2, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18650, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     3, STD, 400,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18651, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     4, STD, 500,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18652, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT2,        1, STD,  20, 100,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18653, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     5, STD, 100, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18654, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     6, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18655, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     7, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18656, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     8, STD, 400, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18657, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,     9, STD, 500, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18658, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT2,        2, STD,  20, 125,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18659, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    10, STD, 100, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18660, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    11, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18661, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    12, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18662, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    13, STD, 400, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18663, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    14, STD, 500, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18664, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT2,        3, STD,  20, 150,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18665, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    15, STD, 100, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18666, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    16, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18667, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    17, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18668, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    18, STD, 400, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18669, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-TEMP,    19, STD, 500, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "Leaving Chilled Water Temperature",                STD,  LEFT,  250, 258, 1, 0, 0,   0, 0, 3
      LINE,  20, 300, 600, 300, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 270,  95, 410, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18670, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      0, STD, 100, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18671, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      1, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18672, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      2, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18673, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      3, STD, 400, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18674, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-COND-T2,      4, STD, 500, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18675, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT2,        0, STD,  20, 305,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18676, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    0, STD, 100, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18677, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    1, STD, 200, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18678, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    2, STD, 300, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18679, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    3, STD, 400, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18680, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    4, STD, 500, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18681, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT2,        1, STD,  20, 330,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18682, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    5, STD, 100, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18683, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    6, STD, 200, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18684, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    7, STD, 300, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18685, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    8, STD, 400, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18686, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,    9, STD, 500, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18687, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT2,        2, STD,  20, 355,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18688, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   10, STD, 100, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18689, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   11, STD, 200, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18690, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   12, STD, 300, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18691, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   13, STD, 400, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18692, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   14, STD, 500, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18693, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CHWT2,        3, STD,  20, 380,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18694, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   15, STD, 100, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18695, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   16, STD, 200, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18696, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   17, STD, 300, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18697, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   18, STD, 400, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18698, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NTEMP,   19, STD, 500, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""


     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18699, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18700, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18701, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18702, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18703, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18704, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
     

   ENDCASE


   CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 2, 1, 2  ; DX Cooling and heatpump
   
     LABEL, "Cooling Power = f(EDB,ODB) - User Data", BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
     LABEL, "Entering Wetbulb Temperature",              STD,  LEFT,  150, 28, 1, 0, 0,   0, 0, 3
     LABEL, "Outdoor",                                   STD,  LEFT,   25, 41, 1, 0, 0,   0, 0, 3
     LABEL, "DB Temp",                                   STD,  LEFT,   25, 55, 1, 0, 0,   0, 0, 3
      LINE,  20, 70, 400,  70, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 40,  95, 225, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18451, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB2,       0, STD, 100,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18452, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB2,       1, STD, 200,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18453, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB2,       2, STD, 300,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18454, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       0, STD,  20,  75,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18455, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   0, STD, 100,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18456, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   1, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18457, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   2, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18458, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       1, STD,  20, 100,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18459, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   3, STD, 100, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18460, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   4, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18461, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   5, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18462, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       2, STD,  20, 125,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18463, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   6, STD, 100, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18464, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   7, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18465, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   8, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18466, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       3, STD,  20, 150,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18467, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,   9, STD, 100, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18468, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,  10, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18469, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,  11, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18470, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       4, STD,  20, 175,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18471, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,  12, STD, 100, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18472, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,  13, STD, 200, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18473, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,  14, STD, 300, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18474, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       5, STD,  20, 200,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18475, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,  15, STD, 100, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18476, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,  16, STD, 200, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18477, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-TEMP,  17, STD, 300, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "Cooling Power = f(EDB,ODB) - Normalized",  BOLD, LEFT,   15, 240, 1, 0, 0, 400, 0, 3
     LABEL, "Entering Wetbulb Temperature",                STD,  LEFT,  150, 258, 1, 0, 0,   0, 0, 3
     LABEL, "Outdoor",                                     STD,  LEFT,   25, 271, 1, 0, 0,   0, 0, 3
     LABEL, "DB Temp",                                     STD,  LEFT,   25, 285, 1, 0, 0,   0, 0, 3
      LINE,  20, 300, 400, 300, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 270,  95, 455, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18478, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB2,       0, STD, 100, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18479, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB2,       1, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18480, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-EWB2,       2, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18481, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       0, STD,  20, 305,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18482, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  0, STD, 100, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18483, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  1, STD, 200, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18484, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  2, STD, 300, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18485, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       1, STD,  20, 330,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18486, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  3, STD, 100, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18487, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  4, STD, 200, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18488, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  5, STD, 300, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18489, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       2, STD,  20, 355,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18490, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  6, STD, 100, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18491, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  7, STD, 200, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18492, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  8, STD, 300, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18493, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       3, STD,  20, 380,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18494, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP,  9, STD, 100, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18495, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP, 10, STD, 200, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18496, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP, 11, STD, 300, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18497, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       4, STD,  20, 405,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18498, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP, 12, STD, 100, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18499, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP, 13, STD, 200, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18500, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP, 14, STD, 300, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18501, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-ODB2,       5, STD,  20, 430,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18502, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP, 15, STD, 100, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18503, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP, 16, STD, 200, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18504, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NTEMP, 17, STD, 300, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18505, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18506, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18507, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18508, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18509, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18510, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
     
   ENDCASE

    ;******************************************
    ; Performance Data - Cool EIR PLR Tab
    ;******************************************
    TABPAGE, 3375, 0, 1, 3, NOTIMP, " CoolEIRf(plr) "

   CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 2, 3, 4  ; chillers
   

   CASE, PERFORMANCE-DATA, 0, VARIABLE-SPEED, -1, =, 1, 1  ; variable speed

     LABEL, "Water Chiller Power = f(PLR,[ChWT-LIFT]) - User Data",    BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
     LABEL, "Leaving",                                     STD,  LEFT,   25, 41, 1, 0, 0,   0, 0, 3
     LABEL, "ChWT-LIFT",                                     STD,  LEFT,   25, 55, 1, 0, 0,   0, 0, 3
     LABEL, "Water Chiller Power = f(PLR,[ChWT-LIFT]) - Normalized",   BOLD, LEFT,   15, 240, 1, 0, 0, 400, 0, 3
     LABEL, "Leaving",                                     STD,  LEFT,   25, 271, 1, 0, 0,   0, 0, 3
     LABEL, "ChWT-LIFT",                                     STD,  LEFT,   25, 285, 1, 0, 0,   0, 0, 3
     LABEL, "Part Load Ratio",                STD,  LEFT,  300, 28, 1, 0, 0,   0, 0, 3
      LINE,  20, 70, 600,  70, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 40,  95, 180, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18711, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      0, STD, 100,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18712, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      1, STD, 200,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18713, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      2, STD, 300,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18714, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      3, STD, 400,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18715, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      4, STD, 500,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18716, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-LIFT ,        0, STD,  20,  75,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18717, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     0, STD, 100,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18718, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     1, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18719, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     2, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18720, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     3, STD, 400,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18721, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     4, STD, 500,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18722, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-LIFT ,        1, STD,  20, 100,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18723, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     5, STD, 100, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18724, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     6, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18725, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     7, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18726, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     8, STD, 400, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18727, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     9, STD, 500, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18728, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-LIFT ,        2, STD,  20, 125,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18729, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    10, STD, 100, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18730, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    11, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18731, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    12, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18732, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    13, STD, 400, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18733, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    14, STD, 500, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18734, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-LIFT ,        3, STD,  20, 150,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18735, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    15, STD, 100, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18736, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    16, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18737, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    17, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18738, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    18, STD, 400, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18739, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,    19, STD, 500, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "Part Load Ratio",                STD,  LEFT,  300, 258, 1, 0, 0,   0, 0, 3
      LINE,  20, 300, 600, 300, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 270,  95, 410, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18740, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      0, STD, 100, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18741, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      1, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18742, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      2, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18743, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      3, STD, 400, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18744, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR,      4, STD, 500, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18745, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-LIFT ,        0, STD,  20, 305,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18746, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    0, STD, 100, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18747, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    1, STD, 200, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18748, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    2, STD, 300, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18749, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    3, STD, 400, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18750, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    4, STD, 500, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18751, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-LIFT ,        1, STD,  20, 330,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18752, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    5, STD, 100, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18753, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    6, STD, 200, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18754, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    7, STD, 300, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18755, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    8, STD, 400, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18756, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    9, STD, 500, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18757, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-LIFT ,        2, STD,  20, 355,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18758, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   10, STD, 100, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18759, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   11, STD, 200, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18760, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   12, STD, 300, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18761, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   13, STD, 400, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18762, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   14, STD, 500, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18763, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-LIFT ,        3, STD,  20, 380,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18764, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   15, STD, 100, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18765, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   16, STD, 200, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18766, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   17, STD, 300, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18767, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   18, STD, 400, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18768, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,   19, STD, 500, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""


     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18769, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18770, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18771, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18772, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18773, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18774, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
     
   ENDCASE
   
   CASE, ELSE
     LABEL, "Water Chiller Power = f(PLR)",    BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
     LABEL, "User Data",               BOLD,  CENTER,  200, 30, 1, 0, 0,   0, 0, 3
     LABEL, "Normalized",              BOLD,  CENTER,  350, 30, 1, 0, 0,   0, 0, 3
     LABEL, "Part Load",                STD,  CENTER,  150, 45, 1, 0, 0,   0, 0, 3
     LABEL, "Ratio",                    STD,  CENTER,  150, 60, 1, 0, 0,   0, 0, 3
     LABEL, "Power"    ,                STD,  CENTER,  250, 45, 1, 0, 0,   0, 0, 3
     LABEL, "(kW)",                     STD,  CENTER,  250, 60, 1, 0, 0,   0, 0, 3
     LABEL, "EIR"      ,                STD,  CENTER,  350, 45, 1, 0, 0,   0, 0, 3
     LABEL, "f(PLR)"   ,                STD,  CENTER,  350, 60, 1, 0, 0,   0, 0, 3

     EDIT, 18781, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR ,     0, STD, 100,  75,  23,  95,  2, 3,  " 1:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18782, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     0, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18783, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    0, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18785, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR ,     1, STD, 100, 100,  23,  95,  2, 3,  " 2:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18786, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     1, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18787, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    1, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18789, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR ,     2, STD, 100, 125,  23,  95,  2, 3,  " 3:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18790, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     2, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18791, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    2, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18793, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR ,     3, STD, 100, 150,  23,  95,  2, 3,  " 4:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18794, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT,     3, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18795, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    3, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18797, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR  ,    4, STD, 100, 175,  23,  95,  2, 3,  " 5:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18798, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT ,    4, STD, 200, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18799, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    4, STD, 300, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18801, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR  ,    5, STD, 100, 200,  23,  95,  2, 3,  " 6:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18802, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT ,    5, STD, 200, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18803, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    5, STD, 300, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
 
     EDIT, 18805, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR  ,    6, STD, 100, 225,  23,  95,  2, 3,  " 7:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18806, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT ,    6, STD, 200, 225,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18807, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    6, STD, 300, 225,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18809, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR  ,    7, STD, 100, 250,  23,  95,  2, 3,  " 8:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18810, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT ,    7, STD, 200, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18811, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    7, STD, 300, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
 
     EDIT, 18813, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR  ,    8, STD, 100, 275,  23,  95,  2, 3,  " 9:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18814, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT ,    8, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18815, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    8, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18816, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-CRV-PLR  ,    9, STD, 100, 300,  23,  95,  2, 3,  "10:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18817, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-LIFT ,    9, STD, 200, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18818, 0, 0, 0, PERFORMANCE-DATA, 3,   CHLR-PWR-NLIFT,    9, STD, 300, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18821, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18822, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18823, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18824, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18825, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18826, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
   ENDCASE
   ENDCASE


   CASE, ELSE 
     LABEL, "Cooling Power = f(PLR)",    BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
     LABEL, "User Data",               BOLD,  CENTER,  200, 30, 1, 0, 0,   0, 0, 3
     LABEL, "Calculated/Normalized",   BOLD,  CENTER,  400, 30, 1, 0, 0,   0, 0, 3
     LABEL, "Cooling"  ,                STD,  CENTER,  150, 45, 1, 0, 0,   0, 0, 3
     LABEL, "Capacity",                 STD,  CENTER,  150, 60, 1, 0, 0,   0, 0, 3
     LABEL, "Power"    ,                STD,  CENTER,  250, 45, 1, 0, 0,   0, 0, 3
     LABEL, "(kW)",                     STD,  CENTER,  250, 60, 1, 0, 0,   0, 0, 3
     LABEL, "Part Load",                STD,  CENTER,  350, 45, 1, 0, 0,   0, 0, 3
     LABEL, "Ratio"    ,                STD,  CENTER,  350, 60, 1, 0, 0,   0, 0, 3
     LABEL, "EIR"      ,                STD,  CENTER,  450, 45, 1, 0, 0,   0, 0, 3
     LABEL, "f(PLR)"   ,                STD,  CENTER,  450, 60, 1, 0, 0,   0, 0, 3

     EDIT, 18831, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    0, STD, 100,  75,  23,  95,  2, 3,  " 1:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18832, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR     0, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18833, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        0, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18834, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   0, STD, 400,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18835, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    1, STD, 100, 100,  23,  95,  2, 3,  " 2:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18836, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR,    1, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18837, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        1, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18838, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   1, STD, 400, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18839, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    2, STD, 100, 125,  23,  95,  2, 3,  " 3:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18840, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR,    2, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18841, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        2, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18842, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   2, STD, 400, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18843, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    3, STD, 100, 150,  23,  95,  2, 3,  " 4:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18844, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR,    3, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18845, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        3, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18846, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   3, STD, 400, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18847, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    4, STD, 100, 175,  23,  95,  2, 3,  " 5:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18848, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR,    4, STD, 200, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18849, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        4, STD, 300, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18850, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   4, STD, 400, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18851, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    5, STD, 100, 200,  23,  95,  2, 3,  " 6:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18852, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR,    5, STD, 200, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18853, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        5, STD, 300, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18854, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   5, STD, 400, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
 
     EDIT, 18855, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    6, STD, 100, 225,  23,  95,  2, 3,  " 7:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18856, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR,    6, STD, 200, 225,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18857, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        6, STD, 300, 225,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18858, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   6, STD, 400, 225,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18859, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    7, STD, 100, 250,  23,  95,  2, 3,  " 8:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18860, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR,    7, STD, 200, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18861, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        7, STD, 300, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18862, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   7, STD, 400, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
 
     EDIT, 18863, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    8, STD, 100, 275,  23,  95,  2, 3,  " 9:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18864, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR,    8, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18865, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        8, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18870, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   8, STD, 400, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18866, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-CAP-PLR,    9, STD, 100, 300,  23,  95,  2, 3,  "10:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18867, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-PLR,    9, STD, 200, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18868, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PLR,        9, STD, 300, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18869, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-CLG-PWR-NPLR,   9, STD, 400, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18871, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18872, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18873, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18874, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18875, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18876, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
   ENDCASE

    ;******************************************
    ; Performance Data - Heat Capacity Tab
    ;******************************************
    TABPAGE, 3376, 0, 1, 3, NOTIMP, " HeatCapf(t) "

   CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 3, 1, 3, 4  ; COEFFICIENTS
      LABEL, "This tab is only used if TYPE  = 'DX-HEAT-PUMP'.", STD, LEFT, 40, 40, 1, 0, 0, 0, 0, 3
   ENDCASE
   
   CASE, ELSE   ; 
   
     LABEL, "Heating Capacity = f(EDB,ODB) - User Data", BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
     LABEL, "Entering Drybulb Temperature",              STD,  LEFT,  150, 28, 1, 0, 0,   0, 0, 3
     LABEL, "Outdoor",                                   STD,  LEFT,   25, 41, 1, 0, 0,   0, 0, 3
     LABEL, "DB Temp",                                   STD,  LEFT,   25, 55, 1, 0, 0,   0, 0, 3
      LINE,  20, 70, 400,  70, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 40,  95, 225, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18322, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB1,       0, STD, 100,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18323, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB1,       1, STD, 200,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18324, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB1,       2, STD, 300,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18325, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       0, STD,  20,  75,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18326, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   0, STD, 100,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18327, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   1, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18328, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   2, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18329, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       1, STD,  20, 100,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18330, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   3, STD, 100, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18331, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   4, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18332, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   5, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18333, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       2, STD,  20, 125,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18334, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   6, STD, 100, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18335, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   7, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18336, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   8, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18337, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       3, STD,  20, 150,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18338, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,   9, STD, 100, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18339, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,  10, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18340, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,  11, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18341, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       4, STD,  20, 175,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18342, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,  12, STD, 100, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18343, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,  13, STD, 200, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18344, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,  14, STD, 300, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18345, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       5, STD,  20, 200,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18346, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,  15, STD, 100, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18347, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,  16, STD, 200, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18348, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-TEMP,  17, STD, 300, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "Heating Capacity = f(EDB,ODB) - Normalized",  BOLD, LEFT,   15, 240, 1, 0, 0, 400, 0, 3
     LABEL, "Entering Drybulb Temperature",                STD,  LEFT,  150, 258, 1, 0, 0,   0, 0, 3
     LABEL, "Outdoor",                                     STD,  LEFT,   25, 271, 1, 0, 0,   0, 0, 3
     LABEL, "DB Temp",                                     STD,  LEFT,   25, 285, 1, 0, 0,   0, 0, 3
      LINE,  20, 300, 400, 300, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 270,  95, 455, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18352, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB1,       0, STD, 100, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18353, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB1,       1, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18354, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB1,       2, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18355, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       0, STD,  20, 305,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18356, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  0, STD, 100, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18357, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  1, STD, 200, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18358, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  2, STD, 300, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18359, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       1, STD,  20, 330,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18360, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  3, STD, 100, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18361, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  4, STD, 200, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18362, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  5, STD, 300, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18363, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       2, STD,  20, 355,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18364, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  6, STD, 100, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18365, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  7, STD, 200, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18366, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  8, STD, 300, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18367, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       3, STD,  20, 380,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18368, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP,  9, STD, 100, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18369, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP, 10, STD, 200, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18370, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP, 11, STD, 300, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18371, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       4, STD,  20, 405,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18372, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP, 12, STD, 100, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18373, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP, 13, STD, 200, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18374, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP, 14, STD, 300, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18375, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB1,       5, STD,  20, 430,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18376, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP, 15, STD, 100, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18377, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP, 16, STD, 200, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18378, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-NTEMP, 17, STD, 300, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18379, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18380, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18381, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18382, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18383, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18384, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
     
   ENDCASE

    ;******************************************
    ; Performance Data - Heat EIR f(t) Tab
    ;******************************************
    TABPAGE, 3377, 0, 1, 3, NOTIMP, " HeatEIRf(t) "

   CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 3, 1, 3, 4  ; COEFFICIENTS
      LABEL, "This tab is only used if TYPE  = 'DX-HEAT-PUMP'.", STD, LEFT, 40, 40, 1, 0, 0, 0, 0, 3
   ENDCASE
   
   CASE, ELSE   ; 
   
     LABEL, "Heating Power = f(EDB,ODB) - User Data", BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
     LABEL, "Entering Drybulb Temperature",              STD,  LEFT,  150, 28, 1, 0, 0,   0, 0, 3
     LABEL, "Outdoor",                                   STD,  LEFT,   25, 41, 1, 0, 0,   0, 0, 3
     LABEL, "DB Temp",                                   STD,  LEFT,   25, 55, 1, 0, 0,   0, 0, 3
      LINE,  20, 70, 400,  70, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 40,  95, 225, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18512, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB2,       0, STD, 100,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18513, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB2,       1, STD, 200,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18514, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB2,       2, STD, 300,  45,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18515, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       0, STD,  20,  75,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18516, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   0, STD, 100,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18517, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   1, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18518, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   2, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18519, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       1, STD,  20, 100,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18520, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   3, STD, 100, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18521, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   4, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18522, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   5, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18523, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       2, STD,  20, 125,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18524, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   6, STD, 100, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18525, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   7, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18526, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   8, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18527, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       3, STD,  20, 150,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18528, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,   9, STD, 100, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18529, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,  10, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18530, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,  11, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18531, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       4, STD,  20, 175,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18532, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,  12, STD, 100, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18533, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,  13, STD, 200, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18534, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,  14, STD, 300, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18535, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       5, STD,  20, 200,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18536, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,  15, STD, 100, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18537, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,  16, STD, 200, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18538, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-TEMP,  17, STD, 300, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "Heating Power = f(EDB,ODB) - Normalized",  BOLD, LEFT,   15, 240, 1, 0, 0, 400, 0, 3
     LABEL, "Entering Drybulb Temperature",                STD,  LEFT,  150, 258, 1, 0, 0,   0, 0, 3
     LABEL, "Outdoor",                                     STD,  LEFT,   25, 271, 1, 0, 0,   0, 0, 3
     LABEL, "DB Temp",                                     STD,  LEFT,   25, 285, 1, 0, 0,   0, 0, 3
      LINE,  20, 300, 400, 300, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
      LINE,  95, 270,  95, 455, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

     EDIT, 18542, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB2,       0, STD, 100, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18543, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB2,       1, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18544, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-EDB2,       2, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18545, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       0, STD,  20, 305,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18546, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  0, STD, 100, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18547, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  1, STD, 200, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18548, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  2, STD, 300, 305,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18549, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       1, STD,  20, 330,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18550, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  3, STD, 100, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18551, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  4, STD, 200, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18552, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  5, STD, 300, 330,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18553, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       2, STD,  20, 355,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18554, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  6, STD, 100, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18555, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  7, STD, 200, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18556, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  8, STD, 300, 355,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18557, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       3, STD,  20, 380,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18558, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  9, STD, 100, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18559, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP,  0, STD, 200, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18560, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP, 11, STD, 300, 380,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18561, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       4, STD,  20, 405,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18562, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP, 12, STD, 100, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18563, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP, 13, STD, 200, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18564, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP, 14, STD, 300, 405,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     EDIT, 18565, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-ODB2,       5, STD,  20, 430,  23,  55,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""
     EDIT, 18566, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP, 15, STD, 100, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18567, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP, 16, STD, 200, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18568, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NTEMP, 17, STD, 300, 430,  23,  95,  2, 3,  "",  LEFT,  0, 0, 1, LEFT, 4, 5, ""

     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18569, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18570, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18571, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18572, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18573, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18574, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
     
   ENDCASE

    ;******************************************
    ; Performance Data - Heat EIR f(plr) Tab
    ;******************************************
    TABPAGE, 3378, 0, 1, 3, NOTIMP, " HeatEIRf(plr) "

   CASE, PERFORMANCE-DATA, 0, TYPE, -1, =, 3, 1, 3, 4  ; COEFFICIENTS
      LABEL, "This tab is only used if TYPE  = 'DX-HEAT-PUMP'.", STD, LEFT, 40, 40, 1, 0, 0, 0, 0, 3
   ENDCASE
   
   CASE, ELSE   ; 
     LABEL, "Heating Power = f(PLR)",    BOLD, LEFT,   15, 10, 1, 0, 0, 400, 0, 3
     LABEL, "User Data",               BOLD,  CENTER,  200, 30, 1, 0, 0,   0, 0, 3
     LABEL, "Calculated/Normalized",   BOLD,  CENTER,  400, 30, 1, 0, 0,   0, 0, 3
     LABEL, "Cooling"  ,                STD,  CENTER,  150, 45, 1, 0, 0,   0, 0, 3
     LABEL, "Capacity",                 STD,  CENTER,  150, 60, 1, 0, 0,   0, 0, 3
     LABEL, "Power"    ,                STD,  CENTER,  250, 45, 1, 0, 0,   0, 0, 3
     LABEL, "(kW)",                     STD,  CENTER,  250, 60, 1, 0, 0,   0, 0, 3
     LABEL, "Part Load",                STD,  CENTER,  350, 45, 1, 0, 0,   0, 0, 3
     LABEL, "Ratio"    ,                STD,  CENTER,  350, 60, 1, 0, 0,   0, 0, 3
     LABEL, "EIR"      ,                STD,  CENTER,  450, 45, 1, 0, 0,   0, 0, 3
     LABEL, "f(PLR)"   ,                STD,  CENTER,  450, 60, 1, 0, 0,   0, 0, 3

     EDIT, 18881, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    0, STD, 100,  75,  23,  95,  2, 3,  " 1:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18882, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR     0, STD, 200,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18883, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        0, STD, 300,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18884, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   0, STD, 400,  75,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18885, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    1, STD, 100, 100,  23,  95,  2, 3,  " 2:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18886, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR,    1, STD, 200, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18887, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        1, STD, 300, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18888, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   1, STD, 400, 100,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18889, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    2, STD, 100, 125,  23,  95,  2, 3,  " 3:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18890, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR,    2, STD, 200, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18891, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        2, STD, 300, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18892, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   2, STD, 400, 125,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18893, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    3, STD, 100, 150,  23,  95,  2, 3,  " 4:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18894, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR,    3, STD, 200, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18895, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        3, STD, 300, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18896, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   3, STD, 400, 150,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18897, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    4, STD, 100, 175,  23,  95,  2, 3,  " 5:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18898, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR,    4, STD, 200, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18899, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        4, STD, 300, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18900, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   4, STD, 400, 175,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18901, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    5, STD, 100, 200,  23,  95,  2, 3,  " 6:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18902, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR,    5, STD, 200, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18903, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        5, STD, 300, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18904, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   5, STD, 400, 200,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
 
     EDIT, 18905, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    6, STD, 100, 225,  23,  95,  2, 3,  " 7:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18906, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR,    6, STD, 200, 225,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18907, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        6, STD, 300, 225,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18908, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   6, STD, 400, 225,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18909, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    7, STD, 100, 250,  23,  95,  2, 3,  " 8:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18910, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR,    7, STD, 200, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18911, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        7, STD, 300, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18912, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   7, STD, 400, 250,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
 
     EDIT, 18913, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    8, STD, 100, 275,  23,  95,  2, 3,  " 9:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18914, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR,    8, STD, 200, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18915, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        8, STD, 300, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18920, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   8, STD, 400, 275,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     EDIT, 18916, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-CAP-PLR,    9, STD, 100, 300,  23,  95,  2, 3,  "10:",  LEFT,  -25, 0, 0, LEFT, 4, 5, ""
     EDIT, 18917, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-PLR,    9, STD, 200, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18918, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PLR,        9, STD, 300, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""
     EDIT, 18919, 0, 0, 0, PERFORMANCE-DATA, 3,   DX-HTG-PWR-NPLR,   9, STD, 400, 300,  23,  95,  2, 3,  "",  LEFT,  0, 0, 0, LEFT, 4, 5, ""

     LABEL, "DOE-2 Performance Curve - Calculated",  BOLD, LEFT,   15, 470, 1, 0, 0, 580, 0, 3
      LABEL, "Curve Formula:", STD, LEFT,  60, 495, 1, 0, 0, 0, 0, 3
      LABEL, "Where:",         STD, LEFT, 108, 525, 1, 0, 0, 0, 0, 3
      LABEL, "Z = a + bX + cX² + dY + eY² + fXY", STD, LEFT, 170, 495, 1, 0, 0, 0, 0, 3

; keyword referenced here is only a TEMPORARY PLACEHOLDER
     EDIT, 18921, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  0, STD, 200, 520,  23,  90,  8, 3, "a =",  LEFT, -30, 5, 0, LEFT, 4, 5, "First curve formula coefficient"
     EDIT, 18922, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  1, STD, 345, 520,  23,  90,  8, 3, "b =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Second curve formula coefficient"
     EDIT, 18923, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  2, STD, 490, 520,  23,  90,  8, 3, "c =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Third curve formula coefficient"
     EDIT, 18924, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  3, STD, 200, 545,  23,  90,  8, 3, "d =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fourth curve formula coefficient"
     EDIT, 18925, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  4, STD, 345, 545,  23,  90,  8, 3, "e =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Fifth curve formula coefficient"
     EDIT, 18926, 0, 0, 1, PERFORMANCE-DATA, 0, DX-HTG-CAP-TEMP,  5, STD, 490, 545,  23,  90,  8, 3, "f =",  LEFT, -30, 5, 0, LEFT, 4, 5, "Sixth curve formula coefficient"
   ENDCASE


 ;********************************************************************
 ;********************************************************************
 ;**
 ;**		Master Meters Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************
MODTABDLG, 3152, 32079, 1, 100, 100, 470, 710, 0, MASTER-METERS, "Master Meters Properties", NOTIMP, 0, NOTIMP, 0

    EDIT, 14912, 63007, 0, 1, MASTER-METERS, 0,       NAME, -1, STD, 145,  15,  23, 250, 32, 3, "Master Meters Name:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Name of master meters; right mouse quick menu options allow deleting, copying, linking and saving to library"

    ;******************************************
    ; Master Meters - Electric Meters Page
    ;******************************************
    TABPAGE, 3153, 32079, 1, 3, NOTIMP, " Electric Meters "

   COMBO, 14913, 63008, 0, 1, MASTER-METERS, 0,  MSTR-ELEC-METER,    0, STD, 150,  15, 200, 165, 19, 3,  "Master Electric Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "The ultimate default electric meter: all unassigned electricity consumption appears here"

   COMBO, 14914, 63009, 0, 1, MASTER-METERS, 0,  LIGHT-ELEC-METER,   0, STD, 150,  50, 200, 165, 19, 3,         "Lighting Meter:",  LEFT, -110, 5, 0, LEFT, 4, 5, "All unassigned non-task-lighting electric consumption is assigned to this meter (if defined)"
   COMBO, 14915, 63010, 0, 1, MASTER-METERS, 0,  TASK-ELEC-METER,    0, STD, 150,  75, 200, 165, 19, 3,       "Task Light Meter:",  LEFT, -110, 5, 0, LEFT, 4, 5, "All unassigned task-lighting electric consumption is assigned to this meter (if defined)"
   COMBO, 14916, 63011, 0, 1, MASTER-METERS, 0,  EQUIP-ELEC-METER,   0, STD, 150, 100, 200, 165, 19, 3,        "Equipment Meter:",  LEFT, -110, 5, 0, LEFT, 4, 5, "All unassigned equipment electric consumption is assigned to this meter (if defined)"
   COMBO, 14917, 63012, 0, 1, MASTER-METERS, 0,  SOURCE-ELEC-METE,   0, STD, 150, 125, 200, 165, 19, 3,           "Source Meter:",  LEFT, -110, 5, 0, LEFT, 4, 5, "All unassigned 'source' electric consumption is assigned to this meter (if defined)"
   COMBO, 14918, 63013, 0, 1, MASTER-METERS, 0,  HEAT-ELEC-METER,    0, STD, 150, 150, 200, 165, 19, 3,          "Heating Meter:",  LEFT, -110, 5, 0, LEFT, 4, 5, "All unassigned space heating electric consumption is assigned to this meter (if defined)"
   COMBO, 14919, 63014, 0, 1, MASTER-METERS, 0,  COOL-ELEC-METER,    0, STD, 150, 175, 200, 165, 19, 3,          "Cooling Meter:",  LEFT, -110, 5, 0, LEFT, 4, 5, "All unassigned space cooling electric consumption is assigned to this meter (if defined)"

   COMBO, 14920, 63015, 0, 1, MASTER-METERS, 0,  HTREJ-ELEC-METER,   0, STD, 480,  50, 200, 165, 19, 3,        "Heat Rej. Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned heat rejection electric consumption is assigned to this meter (if defined)"
   COMBO, 14921, 63016, 0, 1, MASTER-METERS, 0,  AUX-ELEC-METER,     0, STD, 480,  75, 200, 165, 19, 3,        "Auxiliary Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned auxiliary electric consumption is assigned to this meter (if defined)"
   COMBO, 14922, 63017, 0, 1, MASTER-METERS, 0,  VENT-ELEC-METER,    0, STD, 480, 100, 200, 165, 19, 3,      "Ventilation Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned fan electric consumption is assigned to this meter (if defined)"
   COMBO, 14923, 63018, 0, 1, MASTER-METERS, 0,  REFG-ELEC-METER,    0, STD, 480, 125, 200, 165, 19, 3,    "Refrigeration Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned case refrigeration electric consumption is assigned to this meter (if defined)"
   COMBO, 14924, 63019, 0, 1, MASTER-METERS, 0,  SUPP-ELEC-METER,    0, STD, 480, 150, 200, 165, 19, 3,     "Supplemental Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned supplemental electric space heating consumption is assigned to this meter"
   COMBO, 14925, 63020, 0, 1, MASTER-METERS, 0,  DHW-ELEC-METER,     0, STD, 480, 175, 200, 165, 19, 3,       "DHW Heater Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned DHW electric consumption is assigned to this meter"

; SAC 9/21/04 - added spreadsheet providing access to new EXCLUDE-FROM-TDV keyword array
   LABEL, "Exclude From TDV", STD, LEFT, 30, 220, 1, 0, 0, 270, 0, 3
  SPREAD, 17870, 32079, 0, 1, 0, PowerDOE, 0, MstMtrExclTDVSpread,   0, STD,  45, 240, 100, 225, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""

    ;******************************************
    ; Master Meters - Fuel Meters Page
    ;******************************************
    TABPAGE, 3154, 32079, 1, 3, NOTIMP, " Fuel Meters "

   COMBO, 14926, 63027, 0, 1, MASTER-METERS, 0,  MSTR-FUEL-METER,    0, STD, 150,  15, 200, 165, 19, 3,   "Master Fuel Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "The ultimate default fuel meter: all unassigned fuel consumption appears here"

   COMBO, 14927, 63028, 0, 1, MASTER-METERS, 0,  SOURCE-FUEL-METE,   0, STD, 150,  50, 200, 165, 19, 3,        "Source Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned 'source' fuel consumption is assigned to this meter (if defined)"
   COMBO, 14928, 63029, 0, 1, MASTER-METERS, 0,  HEAT-FUEL-METER,    0, STD, 150,  75, 200, 165, 19, 3,       "Heating Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned space heating fuel consumption is assigned to this meter (if defined)"
   COMBO, 14929, 63030, 0, 1, MASTER-METERS, 0,  COOL-FUEL-METER,    0, STD, 150, 100, 200, 165, 19, 3,       "Cooling Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned space cooling fuel consumption is assigned to this meter (if defined)"
   COMBO, 14930, 63031, 0, 1, MASTER-METERS, 0,  SUPP-FUEL-METER,    0, STD, 150, 125, 200, 165, 19, 3,  "Supplemental Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned supplemental space heating fuel consumption is assigned to this meter"
   COMBO, 14931, 63032, 0, 1, MASTER-METERS, 0,  DHW-FUEL-METER,     0, STD, 150, 150, 200, 165, 19, 3,    "DHW Heater Meter:",  LEFT, -130, 5, 0, LEFT, 4, 5, "All unassigned DHW fuel consumption is assigned to this meter (if defined)"

; SAC 9/21/04 - added spreadsheet providing access to new EXCLUDE-FROM-TDV keyword array
   LABEL, "Exclude From TDV", STD, LEFT, 30, 220, 1, 0, 0, 270, 0, 3
  SPREAD, 17871, 32079, 0, 1, 0, PowerDOE, 0, MstMtrExclTDVSpread,   0, STD,  45, 240, 100, 225, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""



 ;********************************************************************
 ;********************************************************************
 ;**
 ;**     Electric Meter Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************
MODTABDLG, 3107, 32075, 1, 100, 100, 470, 710, 0, ELEC-METER, "Electric Meter Properties", NOTIMP, 0, NOTIMP, 0
 
   COMBO, 14120, 14120, 32075, 1, ELEC-METER, 0, NAME,  0, STD, 205,  15, 400, 250, 19, 3, "Currently Active Electric Meter:",  LEFT, -190, 5, 0, LEFT, 4, 5, "List of all electric meters defined in project; also allows library retrieval and creation"
   STATIC, 1, ELEC-METER, 0, TYPE, 0, 0, 0, 475, 20, 250, STD, LEFT, "Type: ",   "", 0, 3

   ;*****************************************
   ; Basic Specifications 
   ;*****************************************
   TABPAGE, 3108, 32075, 1, 3, NOTIMP, " Basic Specifications "

    EDIT, 14135, 14135, 32075, 1, ELEC-METER, 0,             NAME,  0, STD, 150,  10,  23, 250, 32, 3, "Electric Meter Name:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Name of electric meter; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 14121, 14121, 32075, 1, ELEC-METER, 0,             TYPE,  0, STD, 150,  35, 300, 250, 19, 3,                "Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "Utility=main site meter;Building=attached to Utility Meter;Sub-Meter=Attached to Bldg Meter"
 
   LABEL, "Equipment Efficiency", STD, LEFT, 25, 80, 1, 0, 0, 255, 14158, 3
    EDIT, 14158, 14158, 32075, 1, ELEC-METER, 0,  SOURCE-SITE-EFF, -1, STD, 155, 100,  23,  45,  2, 3,  "Source-to-Site Eff:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Fraction of total energy used at the utility source that arrives at the site boundary"

   LABEL, "Transformer", STD, LEFT, 25, 155, 1, 0, 0, 255, 14159, 3
    EDIT, 14159, 14159, 32075, 1, ELEC-METER, 0, TRANSFORMER-SIZE, -1, STD, 155, 175,  23,  45,  0, 3,                "Size:",  LEFT,  -90,   5, 1, LEFT, 4, 5, "Capacity of this meter's transformer"
    EDIT, 14160, 14160, 32075, 1, ELEC-METER, 0, TRANSFORMER-LOSS, -1, STD, 155, 200,  23,  45,  0, 3,                "Loss:",  LEFT,  -90,   5, 1, LEFT, 4, 5, "Fraction of output power lost at full load (used only if Transformer Size is specified)"
   COMBO, 14171, 14171, 32075, 1, ELEC-METER, 0,  TRANS-LOSS-FPLR,  0, STD,  75, 248, 200, 180, 19, 3, "Losses f(part load):",  LEFT,  -10, -18, 0, LEFT, 4, 5, "Quadratic Curve Fit: Multiplier on the Transformer Loss, as a function of the part load"

   LABEL, "Billing Unit Labels", STD, LEFT, 355, 80, 1, 0, 0, 510, 0, 3
    EDIT, 14137, 14137, 32075, 1, ELEC-METER, 0,       UNIT-INDEX,  0, STD, 470, 100,  23,  40,  0, 3,              "Energy:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the billing unit, used to convert english/metric units"
    EDIT, 14157, 14157, 32075, 1, ELEC-METER, 0,   DEM-UNIT-INDEX,  0, STD, 470, 125,  23,  40,  0, 3,              "Demand:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the maximum demand billing unit"
 
    ; TYPE = UTILITY
    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 1
      LABEL, "Miscellaneous", STD, LEFT, 355, 180, 1, 0, 0, 670, 0, 3
      COMBO, 14932,     0, 32075, 1, ELEC-METER, 1,     METER-REPORT,  0, STD, 470, 200, 120, 200, 19, 3,        "Meter Report:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
      COMBO, 14933,     0, 32075, 1, ELEC-METER, 1,       EQUIP-CTRL,  0, STD, 470, 225, 120, 200, 19, 3,       "Equip Control:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""

      LABEL, "Cogeneration", STD, LEFT, 355, 280, 1, 0, 0, 670, 14934, 3
      COMBO, 14934,     0, 32075, 1, ELEC-METER, 1, COGEN-TRACK-MODE,  0, STD, 470, 300, 120, 200, 19, 3,          "Track Mode:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
      COMBO, 14935,     0, 32075, 1, ELEC-METER, 1,  COGEN-TRACK-SCH,  0, STD, 470, 325, 120, 200, 19, 3,      "Track Schedule:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
    ENDCASE

    ; TYPE = BUILDING
    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 2
      LABEL, "Miscellaneous", STD, LEFT, 355, 180, 1, 0, 0, 670, 0, 3
      COMBO, 14936,     0, 32075, 1, ELEC-METER, 2,     METER-REPORT,  0, STD, 470, 200, 120, 200, 19, 3,        "Meter Report:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
    ENDCASE

    ; TYPE = SUB-METER
    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 3
      LABEL, "Miscellaneous", STD, LEFT, 355, 180, 1, 0, 0, 670, 0, 3
      COMBO, 14937,     0, 32075, 1, ELEC-METER, 3,     METER-REPORT,  0, STD, 470, 200, 120, 200, 19, 3,        "Meter Report:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
    ENDCASE

    ; TYPE = ELECTRIC-SALE
    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 4
      LABEL, "Cogeneration", STD, LEFT, 355, 280, 1, 0, 0, 670, 14938, 3
      COMBO, 14938,     0, 32075, 1, ELEC-METER, 4, COGEN-TRACK-MODE,  0, STD, 470, 300, 120, 200, 19, 3,          "Track Mode:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
      COMBO, 14939,     0, 32075, 1, ELEC-METER, 4,  COGEN-TRACK-SCH,  0, STD, 470, 325, 120, 200, 19, 3,      "Track Schedule:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
    ENDCASE

;SAC 2/16/99 - no need for individual CASE statements - especially since the original command TYPE values weren't set right in the first place
;    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 1
;      LABEL, "Billing Unit Labels", STD, LEFT, 10, 216, 1, 0, 0, 0, 0, 3
;       EDIT, 14137, 14137, 32075, 1, ELEC-METER, 0,       UNIT-INDEX,  0, STD,  90, 243,  23,  40,  0, 3,              "Energy:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the billing unit, used to convert english/metric units"
;       EDIT, 14157, 14157, 32075, 1, ELEC-METER, 0,   DEM-UNIT-INDEX,  0, STD,  90, 268,  23,  40,  0, 3,              "Demand:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the maximum demand billing unit"
;    
;     SPREAD, 11611, 11611, 0, 1, 0, PowerDOE, 0, Elec1Sub,  0, SMALL,  210, 60, 125, 167, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
;    
;      LABEL, "Equipment Efficiency", STD, LEFT, 395, 60, 1, 0, 0, 0, 0, 3
;       EDIT, 14158, 14158, 32075, 1, ELEC-METER, 0,  SOURCE-SITE-EFF, -1, STD,  515,  87,  23,  40,  2, 3, "Source-to-Site Eff:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Fraction of total energy used at the utility source that arrives at the site boundary"
;   
;      LABEL, "Transformer", STD, LEFT, 395, 150, 1, 0, 0, 0, 0, 3
;       EDIT, 14159, 14159, 32075, 1, ELEC-METER, 0, TRANSFORMER-SIZE, -1, STD,  515, 177,  23,  40,  0, 3,                "Transformer Size:",  LEFT, -120,   5, 1, LEFT, 4, 5, "Capacity of this meter's transformer"
;       EDIT, 14160, 14160, 32075, 1, ELEC-METER, 0, TRANSFORMER-LOSS, -1, STD,  515, 202,  23,  40,  0, 3,                "Transformer Loss:",  LEFT, -120,   5, 1, LEFT, 4, 5, "Fraction of output power lost at full load (used only if Transformer Size is specified)"
;      COMBO, 14171, 14171, 32075, 1, ELEC-METER, 0,  TRANS-LOSS-FPLR,  0, STD,  405, 247, 200, 180, 19, 3, "Transformer Losses f(part load):",  LEFT,  -10, -18, 0, LEFT, 4, 5, "Quadratic Curve Fit: Multiplier on the Transformer Loss, as a function of the part load"
;    ENDCASE
; 
;    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 2
;      LABEL, "Billing Unit Labels", STD, LEFT, 10, 216, 1, 0, 0, 0, 0, 3
;       EDIT, 14161, 14137, 32075, 1, ELEC-METER, 0,       UNIT-INDEX,  0, STD,  90, 243,  23,  40,  0, 3,              "Energy:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the billing unit, used to convert english/metric units"
;       EDIT, 14162, 14157, 32075, 1, ELEC-METER, 0,   DEM-UNIT-INDEX,  0, STD,  90, 268,  23,  40,  0, 3,              "Demand:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the maximum demand billing unit"
;    
;     SPREAD, 11612, 11612, 0, 1, 0, PowerDOE, 0, Elec2Bldg,  0, SMALL,  210, 60, 125, 167, 20, 3, "", LEFT,   0,  0, 0, LEFT, 0, 0, ""
;    
;      LABEL, "Equipment Efficiency", STD, LEFT, 395, 60, 1, 0, 0, 0, 0, 3
;       EDIT, 14163, 14158, 32075, 1, ELEC-METER, 0,  SOURCE-SITE-EFF, -1, STD,  515,  87,  23,  40,  2, 3, "Source-to-Site Eff:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Fraction of total energy used at the utility source that arrives at the site boundary"
;   
;      LABEL, "Transformer", STD, LEFT, 395, 150, 1, 0, 0, 0, 0, 3
;       EDIT, 14164, 14159, 32075, 1, ELEC-METER, 0, TRANSFORMER-SIZE, -1, STD,  515, 177,  23,  40,  0, 3,                "Transformer Size:",  LEFT, -120,   5, 1, LEFT, 4, 5, "Capacity of this meter's transformer"
;       EDIT, 14165, 14160, 32075, 1, ELEC-METER, 0, TRANSFORMER-LOSS, -1, STD,  515, 202,  23,  40,  0, 3,                "Transformer Loss:",  LEFT, -120,   5, 1, LEFT, 4, 5, "Fraction of output power lost at full load (used only if Transformer Size is specified)"
;      COMBO, 14172, 14171, 32075, 1, ELEC-METER, 0,  TRANS-LOSS-FPLR,  0, STD,  405, 247, 200, 180, 19, 3, "Transformer Losses f(part load):",  LEFT,  -10, -18, 0, LEFT, 4, 5, "Quadratic Curve Fit: Multiplier on the Transformer Loss, as a function of the part load"
;    ENDCASE
; 
;    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 3
;      LABEL, "Billing Unit Labels", STD, LEFT, 10, 216, 1, 0, 0, 0, 0, 3
;       EDIT, 14166, 14137, 32075, 1, ELEC-METER, 0,       UNIT-INDEX,  0, STD,  90, 243,  23,  40,  0, 3,              "Energy:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the billing unit, used to convert english/metric units"
;       EDIT, 14167, 14157, 32075, 1, ELEC-METER, 0,   DEM-UNIT-INDEX,  0, STD,  90, 268,  23,  40,  0, 3,              "Demand:",  LEFT,  -70, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the maximum demand billing unit"
;    
;      LABEL, "Equipment Efficiency", STD, LEFT, 395, 60, 1, 0, 0, 0, 0, 3
;       EDIT, 14168, 14158, 32075, 1, ELEC-METER, 0,  SOURCE-SITE-EFF, -1, STD,  515,  87,  23,  40,  2, 3, "Source-to-Site Eff:",  LEFT, -120, 5, 1, LEFT, 4, 5, "Fraction of total energy used at the utility source that arrives at the site boundary"
;   
;      LABEL, "Transformer", STD, LEFT, 395, 150, 1, 0, 0, 0, 0, 3
;       EDIT, 14169, 14159, 32075, 1, ELEC-METER, 0, TRANSFORMER-SIZE, -1, STD,  515, 177,  23,  40,  0, 3,                "Transformer Size:",  LEFT, -120,   5, 1, LEFT, 4, 5, "Capacity of this meter's transformer"
;       EDIT, 14170, 14160, 32075, 1, ELEC-METER, 0, TRANSFORMER-LOSS, -1, STD,  515, 202,  23,  40,  0, 3,                "Transformer Loss:",  LEFT, -120,   5, 1, LEFT, 4, 5, "Fraction of output power lost at full load (used only if Transformer Size is specified)"
;      COMBO, 14173, 14171, 32075, 1, ELEC-METER, 0,  TRANS-LOSS-FPLR,  0, STD,  405, 247, 200, 180, 19, 3, "Transformer Losses f(part load):",  LEFT,  -10, -18, 0, LEFT, 4, 5, "Quadratic Curve Fit: Multiplier on the Transformer Loss, as a function of the part load"
;    ENDCASE
 
   ;*****************************************
   ; Building or Sub-Meters
   ;*****************************************
   TABPAGE, 3155, 32075, 1, 3, NOTIMP, " Building and/or Submeters "

    ; TYPE = UTILITY
    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 1
      LABEL, "Building and/or Submeters", STD, LEFT, 15, 15, 1, 0, 0, 690, 0, 3
      COMBO, 14940,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  0, STD,  40,  35, 120, 125, 19, 3,   "1:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14941,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  1, STD,  40,  60, 120, 125, 19, 3,   "2:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14942,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  2, STD,  40,  85, 120, 125, 19, 3,   "3:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14943,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  3, STD,  40, 110, 120, 125, 19, 3,   "4:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14944,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  4, STD,  40, 135, 120, 125, 19, 3,   "5:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14945,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  5, STD,  40, 160, 120, 125, 19, 3,   "6:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14946,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  6, STD,  40, 185, 120, 125, 19, 3,   "7:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14947,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  7, STD,  40, 210, 120, 125, 19, 3,   "8:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14948,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  8, STD,  40, 235, 120, 125, 19, 3,   "9:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14949,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS,  9, STD,  40, 260, 120, 125, 19, 3,  "10:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14950,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 10, STD,  40, 285, 120, 125, 19, 3,  "11:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14951,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 11, STD,  40, 310, 120, 125, 19, 3,  "12:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14952,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 12, STD,  40, 335, 120, 125, 19, 3,  "13:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""

      COMBO, 14953,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 13, STD, 215,  35, 120, 125, 19, 3,  "14:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14954,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 14, STD, 215,  60, 120, 125, 19, 3,  "15:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14955,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 15, STD, 215,  85, 120, 125, 19, 3,  "16:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14956,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 16, STD, 215, 110, 120, 125, 19, 3,  "17:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14957,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 17, STD, 215, 135, 120, 125, 19, 3,  "18:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14958,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 18, STD, 215, 160, 120, 125, 19, 3,  "19:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14959,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 19, STD, 215, 185, 120, 125, 19, 3,  "20:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14960,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 20, STD, 215, 210, 120, 125, 19, 3,  "21:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14961,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 21, STD, 215, 235, 120, 125, 19, 3,  "22:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14962,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 22, STD, 215, 260, 120, 125, 19, 3,  "23:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14963,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 23, STD, 215, 285, 120, 125, 19, 3,  "24:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14964,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 24, STD, 215, 310, 120, 125, 19, 3,  "25:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14965,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 25, STD, 215, 335, 120, 125, 19, 3,  "26:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""

      COMBO, 14966,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 26, STD, 390,  35, 120, 125, 19, 3,  "27:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14967,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 27, STD, 390,  60, 120, 125, 19, 3,  "28:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14968,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 28, STD, 390,  85, 120, 125, 19, 3,  "29:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14969,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 29, STD, 390, 110, 120, 125, 19, 3,  "30:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14970,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 30, STD, 390, 135, 120, 125, 19, 3,  "31:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14971,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 31, STD, 390, 160, 120, 125, 19, 3,  "32:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14972,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 32, STD, 390, 185, 120, 125, 19, 3,  "33:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14973,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 33, STD, 390, 210, 120, 125, 19, 3,  "34:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14974,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 34, STD, 390, 235, 120, 125, 19, 3,  "35:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14975,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 35, STD, 390, 260, 120, 125, 19, 3,  "36:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14976,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 36, STD, 390, 285, 120, 125, 19, 3,  "37:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14977,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 37, STD, 390, 310, 120, 125, 19, 3,  "38:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14978,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 38, STD, 390, 335, 120, 125, 19, 3,  "39:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""

      COMBO, 14979,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 39, STD, 565,  35, 120, 125, 19, 3,  "40:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14980,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 40, STD, 565,  60, 120, 125, 19, 3,  "41:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14981,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 41, STD, 565,  85, 120, 125, 19, 3,  "42:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14982,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 42, STD, 565, 110, 120, 125, 19, 3,  "43:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14983,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 43, STD, 565, 135, 120, 125, 19, 3,  "44:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14984,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 44, STD, 565, 160, 120, 125, 19, 3,  "45:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14985,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 45, STD, 565, 185, 120, 125, 19, 3,  "46:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14986,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 46, STD, 565, 210, 120, 125, 19, 3,  "47:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14987,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 47, STD, 565, 235, 120, 125, 19, 3,  "48:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14988,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 48, STD, 565, 260, 120, 125, 19, 3,  "49:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14989,     0, 32075, 1, ELEC-METER, 1, BLDG/SUB-METERS, 49, STD, 565, 285, 120, 125, 19, 3,  "50:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
    ENDCASE
 
    ; TYPE = BUILDING
    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 2
      LABEL, "Submeters", STD, LEFT, 15, 15, 1, 0, 0, 690, 0, 3
      COMBO, 14990,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  0, STD,  40,  35, 120, 125, 19, 3,   "1:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14991,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  1, STD,  40,  60, 120, 125, 19, 3,   "2:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14992,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  2, STD,  40,  85, 120, 125, 19, 3,   "3:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14993,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  3, STD,  40, 110, 120, 125, 19, 3,   "4:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14994,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  4, STD,  40, 135, 120, 125, 19, 3,   "5:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14995,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  5, STD,  40, 160, 120, 125, 19, 3,   "6:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14996,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  6, STD,  40, 185, 120, 125, 19, 3,   "7:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14997,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  7, STD,  40, 210, 120, 125, 19, 3,   "8:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14998,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  8, STD,  40, 235, 120, 125, 19, 3,   "9:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 14999,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS,  9, STD,  40, 260, 120, 125, 19, 3,  "10:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15000,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 10, STD,  40, 285, 120, 125, 19, 3,  "11:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15001,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 11, STD,  40, 310, 120, 125, 19, 3,  "12:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15002,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 12, STD,  40, 335, 120, 125, 19, 3,  "13:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""

      COMBO, 15003,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 13, STD, 215,  35, 120, 125, 19, 3,  "14:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15004,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 14, STD, 215,  60, 120, 125, 19, 3,  "15:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15005,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 15, STD, 215,  85, 120, 125, 19, 3,  "16:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15006,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 16, STD, 215, 110, 120, 125, 19, 3,  "17:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15007,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 17, STD, 215, 135, 120, 125, 19, 3,  "18:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15008,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 18, STD, 215, 160, 120, 125, 19, 3,  "19:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15009,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 19, STD, 215, 185, 120, 125, 19, 3,  "20:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15010,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 20, STD, 215, 210, 120, 125, 19, 3,  "21:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15011,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 21, STD, 215, 235, 120, 125, 19, 3,  "22:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15012,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 22, STD, 215, 260, 120, 125, 19, 3,  "23:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15013,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 23, STD, 215, 285, 120, 125, 19, 3,  "24:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15014,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 24, STD, 215, 310, 120, 125, 19, 3,  "25:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15015,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 25, STD, 215, 335, 120, 125, 19, 3,  "26:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""

      COMBO, 15016,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 26, STD, 390,  35, 120, 125, 19, 3,  "27:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15017,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 27, STD, 390,  60, 120, 125, 19, 3,  "28:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15018,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 28, STD, 390,  85, 120, 125, 19, 3,  "29:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15019,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 29, STD, 390, 110, 120, 125, 19, 3,  "30:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15020,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 30, STD, 390, 135, 120, 125, 19, 3,  "31:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15021,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 31, STD, 390, 160, 120, 125, 19, 3,  "32:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15022,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 32, STD, 390, 185, 120, 125, 19, 3,  "33:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15023,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 33, STD, 390, 210, 120, 125, 19, 3,  "34:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15024,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 34, STD, 390, 235, 120, 125, 19, 3,  "35:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15025,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 35, STD, 390, 260, 120, 125, 19, 3,  "36:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15026,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 36, STD, 390, 285, 120, 125, 19, 3,  "37:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15027,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 37, STD, 390, 310, 120, 125, 19, 3,  "38:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15028,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 38, STD, 390, 335, 120, 125, 19, 3,  "39:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""

      COMBO, 15029,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 39, STD, 565,  35, 120, 125, 19, 3,  "40:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15030,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 40, STD, 565,  60, 120, 125, 19, 3,  "41:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15031,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 41, STD, 565,  85, 120, 125, 19, 3,  "42:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15032,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 42, STD, 565, 110, 120, 125, 19, 3,  "43:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15033,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 43, STD, 565, 135, 120, 125, 19, 3,  "44:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15034,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 44, STD, 565, 160, 120, 125, 19, 3,  "45:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15035,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 45, STD, 565, 185, 120, 125, 19, 3,  "46:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15036,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 46, STD, 565, 210, 120, 125, 19, 3,  "47:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15037,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 47, STD, 565, 235, 120, 125, 19, 3,  "48:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15038,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 48, STD, 565, 260, 120, 125, 19, 3,  "49:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
      COMBO, 15039,     0, 32075, 1, ELEC-METER, 2,      SUB-METERS, 49, STD, 565, 285, 120, 125, 19, 3,  "50:",  LEFT,  -25, 5, 0, LEFT, 4, 5, ""
    ENDCASE
 
    ; TYPE = SUB-METER
    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 3
      LABEL, "No building or submeter assignments when electric meter type = 'Sub-Meter'", STD, LEFT, 20, 20, 1, 0, 0, 0, 0, 3
    ENDCASE
 
    ; TYPE = ELECTRIC-SALE
    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 4
      LABEL, "No building or submeter assignments when electric meter type = 'Electric Sale'", STD, LEFT, 20, 20, 1, 0, 0, 0, 0, 3
    ENDCASE

   ;*****************************************
   ; Direct Loads 
   ;*****************************************
   TABPAGE, 3109, 32075, 1, 3, NOTIMP, " Direct Loads "

;   COMBO, 14131, 14120, 32075, 1, ELEC-METER, 0, NAME, 0, STD, 300,  10, 260, 160, 21, 3, "Currently Active Electric Meter:", RIGHT, 290,  12, 0, LEFT, 355,  34, "Name of electric meter; options allow renaming, deleting, copying, linking, save to library"
;    LINE, 10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3

    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 1
      LABEL, "Interior Direct Loads", STD, LEFT, 25, 15, 1, 0, 0, 515, 0, 3
     SPREAD, 15040,   736, 0, 1, 0, PowerDOE, 0, EMtr1IntLoadsSpread,  0, STD,  40,  35, 100, 475, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
;      LABEL, "Interior Direct Loads", STD, LEFT, 25, 13, 1, 0, 0, 350, 0, 3
;      LABEL, "Load (kW)", STD, CENTER, 105, 32, 1, 0, 0, 0, 15040, 3
;      LABEL, "Schedule",  STD, CENTER, 245, 32, 1, 0, 0, 0, 15041, 3
;       EDIT, 15040,   736, 32075, 1, ELEC-METER, 1, INTERIOR-POWER,  0, STD,  70,  50,  23,  70,  2, 3,   "1:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15041,   735, 32075, 1, ELEC-METER, 1, INTERIOR-SCH,    0, STD, 150,  50, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15042,   736, 32075, 1, ELEC-METER, 1, INTERIOR-POWER,  1, STD,  70,  75,  23,  70,  2, 3,   "2:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15043,   735, 32075, 1, ELEC-METER, 1, INTERIOR-SCH,    1, STD, 150,  75, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15044,   736, 32075, 1, ELEC-METER, 1, INTERIOR-POWER,  2, STD,  70, 100,  23,  70,  2, 3,   "3:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15045,   735, 32075, 1, ELEC-METER, 1, INTERIOR-SCH,    2, STD, 150, 100, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15046,   736, 32075, 1, ELEC-METER, 1, INTERIOR-POWER,  3, STD,  70, 125,  23,  70,  2, 3,   "4:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15047,   735, 32075, 1, ELEC-METER, 1, INTERIOR-SCH,    3, STD, 150, 125, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15048,   736, 32075, 1, ELEC-METER, 1, INTERIOR-POWER,  4, STD,  70, 150,  23,  70,  2, 3,   "5:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15049,   735, 32075, 1, ELEC-METER, 1, INTERIOR-SCH,    4, STD, 150, 150, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"

; SAC 9/21/04 - Repositioned controls and increased width of exterior loads spread to accomodate new EXTERIOR-EU keyword
      LABEL, "Exterior Direct Loads", STD, LEFT, 25, 160, 1, 0, 0, 515, 0, 3
     SPREAD, 15050,   738, 0, 1, 0, PowerDOE, 0, EMtr1ExtLoadsSpread,  0, STD,  40, 180, 100, 475, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
;      LABEL, "Exterior Direct Loads", STD, LEFT, 25, 203, 1, 0, 0, 350, 0, 3
;      LABEL, "Load (kW)", STD, CENTER, 105, 222, 1, 0, 0, 0, 15050, 3
;      LABEL, "Schedule",  STD, CENTER, 245, 222, 1, 0, 0, 0, 15051, 3
;       EDIT, 15050,   738, 32075, 1, ELEC-METER, 1, EXTERIOR-POWER,  0, STD,  70, 240,  23,  70,  2, 3,   "1:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15051,   737, 32075, 1, ELEC-METER, 1, EXTERIOR-SCH,    0, STD, 150, 240, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15052,   738, 32075, 1, ELEC-METER, 1, EXTERIOR-POWER,  1, STD,  70, 265,  23,  70,  2, 3,   "2:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15053,   737, 32075, 1, ELEC-METER, 1, EXTERIOR-SCH,    1, STD, 150, 265, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15054,   738, 32075, 1, ELEC-METER, 1, EXTERIOR-POWER,  2, STD,  70, 290,  23,  70,  2, 3,   "3:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15055,   737, 32075, 1, ELEC-METER, 1, EXTERIOR-SCH,    2, STD, 150, 290, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15056,   738, 32075, 1, ELEC-METER, 1, EXTERIOR-POWER,  3, STD,  70, 315,  23,  70,  2, 3,   "4:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15057,   737, 32075, 1, ELEC-METER, 1, EXTERIOR-SCH,    3, STD, 150, 315, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15058,   738, 32075, 1, ELEC-METER, 1, EXTERIOR-POWER,  4, STD,  70, 340,  23,  70,  2, 3,   "5:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15059,   737, 32075, 1, ELEC-METER, 1, EXTERIOR-SCH,    4, STD, 150, 340, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"

      LABEL, "Refrigeration Direct Loads", STD, LEFT, 25, 305, 1, 0, 0, 295, 0, 3
      LABEL, "Load (kW)", STD, CENTER,  75, 323, 1, 0, 0, 0, 15625, 3
       EDIT, 15625,     0, 32075, 1, ELEC-METER, 1, REFG-POWER,      0, STD,  40, 340,  23,  70,  3, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "Hourly energy consumption of refrigeration equipment (excluding equipment modeled by the simulation)"
      LABEL, "Schedule",  STD, CENTER, 200, 323, 1, 0, 0, 0, 15626, 3
      COMBO, 15626,     0, 32075, 1, ELEC-METER, 1, REFG-SCH,        0, STD, 115, 340, 120, 180, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Refrigeration Load each hour"
;      LABEL, "Refrigeration Direct Loads", STD, LEFT, 410, 203, 1, 0, 0, 680, 0, 3
;      LABEL, "Load (kW)", STD, CENTER, 455, 222, 1, 0, 0, 0, 15625, 3
;       EDIT, 15625,     0, 32075, 1, ELEC-METER, 1, REFG-POWER,      0, STD, 420, 240,  23,  70,  3, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "Hourly energy consumption of refrigeration equipment (excluding equipment modeled by the simulation)"
;      LABEL, "Schedule",  STD, CENTER, 585, 222, 1, 0, 0, 0, 15626, 3
;      COMBO, 15626,     0, 32075, 1, ELEC-METER, 1, REFG-SCH,        0, STD, 500, 240, 120, 180, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Refrigeration Load each hour"
    ENDCASE     

    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 2
      LABEL, "Interior Direct Loads", STD, LEFT, 25, 15, 1, 0, 0, 515, 0, 3
     SPREAD, 15060,   736, 0, 1, 0, PowerDOE, 0, EMtr2IntLoadsSpread,  0, STD,  40,  35, 100, 475, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
;      LABEL, "Interior Direct Loads", STD, LEFT, 25, 13, 1, 0, 0, 350, 0, 3
;      LABEL, "Load (kW)", STD, CENTER, 105, 32, 1, 0, 0, 0, 15060, 3
;      LABEL, "Schedule",  STD, CENTER, 245, 32, 1, 0, 0, 0, 15061, 3
;       EDIT, 15060,   736, 32075, 1, ELEC-METER, 2, INTERIOR-POWER,  0, STD,  70,  50,  23,  70,  2, 3,   "1:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15061,   735, 32075, 1, ELEC-METER, 2, INTERIOR-SCH,    0, STD, 150,  50, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15062,   736, 32075, 1, ELEC-METER, 2, INTERIOR-POWER,  1, STD,  70,  75,  23,  70,  2, 3,   "2:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15063,   735, 32075, 1, ELEC-METER, 2, INTERIOR-SCH,    1, STD, 150,  75, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15064,   736, 32075, 1, ELEC-METER, 2, INTERIOR-POWER,  2, STD,  70, 100,  23,  70,  2, 3,   "3:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15065,   735, 32075, 1, ELEC-METER, 2, INTERIOR-SCH,    2, STD, 150, 100, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15066,   736, 32075, 1, ELEC-METER, 2, INTERIOR-POWER,  3, STD,  70, 125,  23,  70,  2, 3,   "4:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15067,   735, 32075, 1, ELEC-METER, 2, INTERIOR-SCH,    3, STD, 150, 125, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15068,   736, 32075, 1, ELEC-METER, 2, INTERIOR-POWER,  4, STD,  70, 150,  23,  70,  2, 3,   "5:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15069,   735, 32075, 1, ELEC-METER, 2, INTERIOR-SCH,    4, STD, 150, 150, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"

; SAC 9/21/04 - Repositioned controls and increased width of exterior loads spread to accomodate new EXTERIOR-EU keyword
      LABEL, "Exterior Direct Loads", STD, LEFT, 25, 160, 1, 0, 0, 515, 0, 3
     SPREAD, 15070,   738, 0, 1, 0, PowerDOE, 0, EMtr2ExtLoadsSpread,  0, STD,  40, 180, 100, 475, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
;      LABEL, "Exterior Direct Loads", STD, LEFT, 25, 203, 1, 0, 0, 350, 0, 3
;      LABEL, "Load (kW)", STD, CENTER, 105, 222, 1, 0, 0, 0, 15070, 3
;      LABEL, "Schedule",  STD, CENTER, 245, 222, 1, 0, 0, 0, 15071, 3
;       EDIT, 15070,   738, 32075, 1, ELEC-METER, 2, EXTERIOR-POWER,  0, STD,  70, 240,  23,  70,  2, 3,   "1:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15071,   737, 32075, 1, ELEC-METER, 2, EXTERIOR-SCH,    0, STD, 150, 240, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15072,   738, 32075, 1, ELEC-METER, 2, EXTERIOR-POWER,  1, STD,  70, 265,  23,  70,  2, 3,   "2:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15073,   737, 32075, 1, ELEC-METER, 2, EXTERIOR-SCH,    1, STD, 150, 265, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15074,   738, 32075, 1, ELEC-METER, 2, EXTERIOR-POWER,  2, STD,  70, 290,  23,  70,  2, 3,   "3:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15075,   737, 32075, 1, ELEC-METER, 2, EXTERIOR-SCH,    2, STD, 150, 290, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15076,   738, 32075, 1, ELEC-METER, 2, EXTERIOR-POWER,  3, STD,  70, 315,  23,  70,  2, 3,   "4:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15077,   737, 32075, 1, ELEC-METER, 2, EXTERIOR-SCH,    3, STD, 150, 315, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15078,   738, 32075, 1, ELEC-METER, 2, EXTERIOR-POWER,  4, STD,  70, 340,  23,  70,  2, 3,   "5:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15079,   737, 32075, 1, ELEC-METER, 2, EXTERIOR-SCH,    4, STD, 150, 340, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"

      LABEL, "Refrigeration Direct Loads", STD, LEFT, 25, 305, 1, 0, 0, 295, 0, 3
      LABEL, "Load (kW)", STD, CENTER,  75, 323, 1, 0, 0, 0, 15627, 3
       EDIT, 15627,     0, 32075, 1, ELEC-METER, 2, REFG-POWER,      0, STD,  40, 340,  23,  70,  3, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "Hourly energy consumption of refrigeration equipment (excluding equipment modeled by the simulation)"
      LABEL, "Schedule",  STD, CENTER, 200, 323, 1, 0, 0, 0, 15628, 3
      COMBO, 15628,     0, 32075, 1, ELEC-METER, 2, REFG-SCH,        0, STD, 115, 340, 120, 180, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Refrigeration Load each hour"
;      LABEL, "Refrigeration Direct Loads", STD, LEFT, 400, 203, 1, 0, 0, 680, 0, 3
;      LABEL, "Load (kW)", STD, CENTER, 455, 222, 1, 0, 0, 0, 15627, 3
;       EDIT, 15627,     0, 32075, 1, ELEC-METER, 2, REFG-POWER,      0, STD, 420, 240,  23,  70,  3, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "Hourly energy consumption of refrigeration equipment (excluding equipment modeled by the simulation)"
;      LABEL, "Schedule",  STD, CENTER, 585, 222, 1, 0, 0, 0, 15628, 3
;      COMBO, 15628,     0, 32075, 1, ELEC-METER, 2, REFG-SCH,        0, STD, 500, 240, 120, 180, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Refrigeration Load each hour"
    ENDCASE     

    CASE,  ELEC-METER,  0, TYPE,  -1,  =, 1, 3
      LABEL, "Interior Direct Loads", STD, LEFT, 25, 15, 1, 0, 0, 515, 0, 3
     SPREAD, 15080,   736, 0, 1, 0, PowerDOE, 0, EMtr3IntLoadsSpread,  0, STD,  40,  35, 100, 475, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
;      LABEL, "Interior Direct Loads", STD, LEFT, 25, 13, 1, 0, 0, 350, 0, 3
;      LABEL, "Load (kW)", STD, CENTER, 105, 32, 1, 0, 0, 0, 15080, 3
;      LABEL, "Schedule",  STD, CENTER, 245, 32, 1, 0, 0, 0, 15081, 3
;       EDIT, 15080,   736, 32075, 1, ELEC-METER, 3, INTERIOR-POWER,  0, STD,  70,  50,  23,  70,  2, 3,   "1:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15081,   735, 32075, 1, ELEC-METER, 3, INTERIOR-SCH,    0, STD, 150,  50, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15082,   736, 32075, 1, ELEC-METER, 3, INTERIOR-POWER,  1, STD,  70,  75,  23,  70,  2, 3,   "2:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15083,   735, 32075, 1, ELEC-METER, 3, INTERIOR-SCH,    1, STD, 150,  75, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15084,   736, 32075, 1, ELEC-METER, 3, INTERIOR-POWER,  2, STD,  70, 100,  23,  70,  2, 3,   "3:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15085,   735, 32075, 1, ELEC-METER, 3, INTERIOR-SCH,    2, STD, 150, 100, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15086,   736, 32075, 1, ELEC-METER, 3, INTERIOR-POWER,  3, STD,  70, 125,  23,  70,  2, 3,   "4:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15087,   735, 32075, 1, ELEC-METER, 3, INTERIOR-SCH,    3, STD, 150, 125, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;       EDIT, 15088,   736, 32075, 1, ELEC-METER, 3, INTERIOR-POWER,  4, STD,  70, 150,  23,  70,  2, 3,   "5:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15089,   735, 32075, 1, ELEC-METER, 3, INTERIOR-SCH,    4, STD, 150, 150, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"

; SAC 9/21/04 - Repositioned controls and increased width of exterior loads spread to accomodate new EXTERIOR-EU keyword
      LABEL, "Exterior Direct Loads", STD, LEFT, 25, 160, 1, 0, 0, 515, 0, 3
     SPREAD, 15090,   738, 0, 1, 0, PowerDOE, 0, EMtr3ExtLoadsSpread,  0, STD,  40, 180, 100, 475, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
;      LABEL, "Exterior Direct Loads", STD, LEFT, 25, 203, 1, 0, 0, 350, 0, 3
;      LABEL, "Load (kW)", STD, CENTER, 105, 222, 2, 0, 0, 0, 15090, 3
;      LABEL, "Schedule",  STD, CENTER, 245, 222, 2, 0, 0, 0, 15091, 3
;       EDIT, 15090,   738, 32075, 1, ELEC-METER, 3, EXTERIOR-POWER,  0, STD,  70, 240,  23,  70,  2, 3,   "1:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15091,   737, 32075, 1, ELEC-METER, 3, EXTERIOR-SCH,    0, STD, 150, 240, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15092,   738, 32075, 1, ELEC-METER, 3, EXTERIOR-POWER,  1, STD,  70, 265,  23,  70,  2, 3,   "2:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15093,   737, 32075, 1, ELEC-METER, 3, EXTERIOR-SCH,    1, STD, 150, 265, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15094,   738, 32075, 1, ELEC-METER, 3, EXTERIOR-POWER,  2, STD,  70, 290,  23,  70,  2, 3,   "3:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15095,   737, 32075, 1, ELEC-METER, 3, EXTERIOR-SCH,    2, STD, 150, 290, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15096,   738, 32075, 1, ELEC-METER, 3, EXTERIOR-POWER,  3, STD,  70, 315,  23,  70,  2, 3,   "4:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15097,   737, 32075, 1, ELEC-METER, 3, EXTERIOR-SCH,    3, STD, 150, 315, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;       EDIT, 15098,   738, 32075, 1, ELEC-METER, 3, EXTERIOR-POWER,  4, STD,  70, 340,  23,  70,  2, 3,   "5:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;      COMBO, 15099,   737, 32075, 1, ELEC-METER, 3, EXTERIOR-SCH,    4, STD, 150, 340, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"

      LABEL, "Refrigeration Direct Loads", STD, LEFT, 25, 305, 1, 0, 0, 295, 0, 3
      LABEL, "Load (kW)", STD, CENTER,  75, 323, 1, 0, 0, 0, 15629, 3
       EDIT, 15629,     0, 32075, 1, ELEC-METER, 3, REFG-POWER,      0, STD,  40, 340,  23,  70,  3, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "Hourly energy consumption of refrigeration equipment (excluding equipment modeled by the simulation)"
      LABEL, "Schedule",  STD, CENTER, 200, 323, 1, 0, 0, 0, 15630, 3
      COMBO, 15630,     0, 32075, 1, ELEC-METER, 3, REFG-SCH,        0, STD, 115, 340, 120, 180, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Refrigeration Load each hour"
;      LABEL, "Refrigeration Direct Loads", STD, LEFT, 400, 203, 1, 0, 0, 680, 0, 3
;      LABEL, "Load (kW)", STD, CENTER, 455, 222, 1, 0, 0, 0, 15629, 3
;      LABEL, "Schedule",  STD, CENTER, 585, 222, 1, 0, 0, 0, 15630, 3
;       EDIT, 15629,     0, 32075, 1, ELEC-METER, 3, REFG-POWER,      0, STD, 420, 240,  23,  70,  3, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "Hourly energy consumption of refrigeration equipment (excluding equipment modeled by the simulation)"
;      COMBO, 15630,     0, 32075, 1, ELEC-METER, 3, REFG-SCH,        0, STD, 500, 240, 120, 180, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Refrigeration Load each hour"
    ENDCASE     


 
 ;********************************************************************
 ;********************************************************************
 ;**
 ;**     Fuel Meter Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************
MODTABDLG, 3110, 32076, 1, 100, 100, 470, 710, 0, FUEL-METER, "Fuel Meter Properties", NOTIMP, 0, NOTIMP, 0
 
   COMBO, 14132, 14132, 32076, 1, FUEL-METER, 0, NAME,  0, STD, 185,  15, 400, 250, 19, 3, "Currently Active Fuel Meter:",  LEFT, -170, 5, 0, LEFT, 4, 5, "List of all fuel meters defined in project; also allows library retrieval and creation"
   STATIC, 1, FUEL-METER, 0, TYPE, 0, 0, 0, 455, 20, 250, STD, LEFT, "Type: ",   "", 0, 3

   ;*****************************************
   ; Basic Specifications 
   ;*****************************************
   TABPAGE, 3111, 32076, 1, 3, NOTIMP, " Basic Specifications "

    EDIT, 14136, 14136, 0, 1, FUEL-METER, 0,             NAME,  0, STD, 130,  10,  23, 250, 32, 3,     "Fuel Meter Name:",  LEFT, -110, 5, 1, LEFT, 4, 5, "Name of fuel meter; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 14133, 14133, 0, 1, FUEL-METER, 0,             TYPE,  0, STD, 130,  35, 300, 250, 19, 3,                "Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "Utility=main site meter;Building=attached to Utility Meter;Sub-Meter=Attached to Bldg Meter"
 
   LABEL, "Equipment Efficiency", STD, LEFT, 25, 80, 1, 0, 0, 255, 14158, 3
    EDIT, 14177, 14177, 0, 1, FUEL-METER, 0,  SOURCE-SITE-EFF, -1, STD, 155, 100,  23,  55,  2, 3,  "Source-to-Site Eff:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Fraction of total energy used at the utility source that arrives at the site boundary"

   LABEL, "Billing Units", STD, LEFT, 355, 80, 1, 0, 0, 580, 0, 3
    EDIT, 14175, 14175, 0, 1, FUEL-METER, 0,       UNIT-INDEX,  0, STD, 470, 100,  23,  70,  0, 3,        "Energy Label:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the billing unit, used to convert english/metric units"
    EDIT, 14176, 14176, 0, 1, FUEL-METER, 0,   DEM-UNIT-INDEX,  0, STD, 470, 125,  23,  70,  0, 3,        "Demand Label:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "An integer from the units table that defines the maximum demand billing unit"
    EDIT, 14174, 14174, 0, 1, FUEL-METER, 0,      ENERGY/UNIT, -1, STD, 470, 150,  23,  70,  0, 3,       "Thermal Value:",  LEFT,  -95, 5, 1, LEFT, 4, 5, "Number of Btus per billing unit for this meter (e.g. 100,000 for therms)"

   LABEL, "Miscellaneous", STD, LEFT, 355, 205, 1, 0, 0, 580, 0, 3
   COMBO, 15100,     0, 0, 1, FUEL-METER, 0,     METER-REPORT,  0, STD, 470, 225, 120, 110, 19, 3,        "Meter Report:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""

   ;*****************************************
   ; Direct Loads 
   ;*****************************************
   TABPAGE, 3112, 32076, 1, 3, NOTIMP, " Direct Loads "
   
;   COMBO, 14134, 14132, 0, 1, FUEL-METER, 0, NAME, 0, STD, 300,  10, 260, 160, 21, 3, "Currently Active Fuel Meter:", RIGHT, 290,  12, 0, LEFT, 355,  34, "Name of fuel meter; options allow renaming, deleting, copying, linking, save to library"
;    LINE, 10, 40, 590, 40, 2, SOLID, 0, 0, 0, NONE, 1, 0, 0, 3
    
   LABEL, "Interior Direct Loads", STD, LEFT, 25, 35, 1, 0, 0, 535, 0, 3
  SPREAD, 15101,   746, 0, 1, 0, PowerDOE, 0, FMtrIntLoadsSpread,  0, STD,  40,  55, 100, 495, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
;   LABEL, "Interior Direct Loads", STD, LEFT, 25, 13, 1, 0, 0, 350, 0, 3
;   LABEL, "Load (kW)", STD, CENTER, 105, 32, 1, 0, 0, 0, 15040, 3
;   LABEL, "Schedule",  STD, CENTER, 245, 32, 1, 0, 0, 0, 15041, 3
;    EDIT, 15101,   746, 0, 1, FUEL-METER, 0, INTERIOR-POWER,  0, STD,  70,  50,  23,  70,  2, 3,   "1:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15102,   745, 0, 1, FUEL-METER, 0, INTERIOR-SCH,    0, STD, 150,  50, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;    EDIT, 15103,   746, 0, 1, FUEL-METER, 0, INTERIOR-POWER,  1, STD,  70,  75,  23,  70,  2, 3,   "2:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15104,   745, 0, 1, FUEL-METER, 0, INTERIOR-SCH,    1, STD, 150,  75, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;    EDIT, 15105,   746, 0, 1, FUEL-METER, 0, INTERIOR-POWER,  2, STD,  70, 100,  23,  70,  2, 3,   "3:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15106,   745, 0, 1, FUEL-METER, 0, INTERIOR-SCH,    2, STD, 150, 100, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;    EDIT, 15107,   746, 0, 1, FUEL-METER, 0, INTERIOR-POWER,  3, STD,  70, 125,  23,  70,  2, 3,   "4:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15108,   745, 0, 1, FUEL-METER, 0, INTERIOR-SCH,    3, STD, 150, 125, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"
;    EDIT, 15109,   746, 0, 1, FUEL-METER, 0, INTERIOR-POWER,  4, STD,  70, 150,  23,  70,  2, 3,   "5:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15110,   745, 0, 1, FUEL-METER, 0, INTERIOR-SCH,    4, STD, 150, 150, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Interior Direct Load each hour"

; SAC 9/27/04 - Added access to new EXTERIOR-EU keyword
   LABEL, "Exterior Direct Loads", STD, LEFT, 25, 205, 1, 0, 0, 535, 0, 3
  SPREAD, 15111,   738, 0, 1, 0, PowerDOE, 0, FMtrExtLoadsSpread,  0, STD,  40, 225, 100, 495, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
;   LABEL, "Exterior Direct Loads", STD, LEFT, 25, 203, 1, 0, 0, 350, 0, 3
;   LABEL, "Load (kW)", STD, CENTER, 105, 222, 1, 0, 0, 0, 15050, 3
;   LABEL, "Schedule",  STD, CENTER, 245, 222, 1, 0, 0, 0, 15051, 3
;    EDIT, 15111,   748, 0, 1, FUEL-METER, 0, EXTERIOR-POWER,  0, STD,  70, 240,  23,  70,  2, 3,   "1:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15112,   747, 0, 1, FUEL-METER, 0, EXTERIOR-SCH,    0, STD, 150, 240, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;    EDIT, 15113,   748, 0, 1, FUEL-METER, 0, EXTERIOR-POWER,  1, STD,  70, 265,  23,  70,  2, 3,   "2:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15114,   747, 0, 1, FUEL-METER, 0, EXTERIOR-SCH,    1, STD, 150, 265, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;    EDIT, 15115,   748, 0, 1, FUEL-METER, 0, EXTERIOR-POWER,  2, STD,  70, 290,  23,  70,  2, 3,   "3:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15116,   747, 0, 1, FUEL-METER, 0, EXTERIOR-SCH,    2, STD, 150, 290, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;    EDIT, 15117,   748, 0, 1, FUEL-METER, 0, EXTERIOR-POWER,  3, STD,  70, 315,  23,  70,  2, 3,   "4:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15118,   747, 0, 1, FUEL-METER, 0, EXTERIOR-SCH,    3, STD, 150, 315, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"
;    EDIT, 15119,   748, 0, 1, FUEL-METER, 0, EXTERIOR-POWER,  4, STD,  70, 340,  23,  70,  2, 3,   "5:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Hourly energy consumption of misc. energy uses (typically use Loop Process Loads instead)"
;   COMBO, 15120,   747, 0, 1, FUEL-METER, 0, EXTERIOR-SCH,    4, STD, 150, 340, 120, 200, 19, 3,     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "A fractional schedule of multipliers applied to the Exterior Direct Load each hour"



 ;********************************************************************
 ;********************************************************************
 ;**
 ;**     Schedule Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************

 MODTABDLG, 3156, 32001, 1, 30, 30, 470, 710, 0, NOTIMP, "Schedule Properties", NOTIMP, 0, NOTIMP, 0

   ;*****************************************
   ; Annual Schedules Page
   ;*****************************************
   TABPAGE, 3157, 32001, 1, 3, SCHEDULE, " Annual Schedules "

   COMBO, 15121, 0, 0, 1, SCHEDULE, 0, NAME,  0, STD, 240,   5, 400, 250, 19, 3, "Currently Active Schedule:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all schedules defined in project; also allows library retrieval and creation"
   STATIC, 1, SCHEDULE, 0, TYPE, 0, 0, 0, 510, 10, 175, STD, LEFT, "Type: ",   "", 0, 3

    LINE,  20, 40, 685, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

    EDIT, 15122,     0, 0, 1, SCHEDULE, 0,             NAME,  0, STD, 125,  55,  23, 250, 32, 3,     "Schedule Name:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Name of schedule; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 15123, 31540, 0, 1, SCHEDULE, 0,             TYPE,  0, STD, 125,  80, 300, 250, 19, 3,              "Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
; SAC 11/28/07 - keyword removed from BDL
;   COMBO, 15124,     0, 0, 1, SCHEDULE, 0,            GROUP,  0, STD, 125, 105, 120, 250, 19, 3,             "Group:", RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
; SDG 1/15/15 - added access to PHOTOCELL-CTRL keyword
    COMBO, 15124,     0, 0, 1, SCHEDULE, 0,   PHOTOCELL-CTRL,  0, STD, 125, 105, 180, 250, 19, 3,     "Photocell Ctrl:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "whether hourly values in the referenced DAY-SCHEDULEs can be overridden either ON (value = 1.0) or OFF (value = 0.0) according to whether it is day or night"

    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 1
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread1,  0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 2
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread2,  0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 3
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread3,  0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 4
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread4,  0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 5
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread5,  0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 6
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread6,  0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 7
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread7,  0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 8
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread8,  0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 9
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread9,  0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 10
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread10, 0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 11
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread11, 0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     
    CASE,  ELSE
       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread12, 0, STD, 125, 152, 235, 406, 19, 3, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
    ENDCASE     

      BUTTON, 15373, 15373, 0, 1, 94, 11523, STD, 125, 390, 23, 130, 3, "Insert Week", "Insert week schedule before the currently highlighted schedule in the list"
      BUTTON, 15372, 15372, 0, 1, 93, 11523, STD, 263, 390, 23, 130, 3, "Add Week",    "Add week schedule onto end of week schedule list"
      BUTTON, 15374, 15374, 0, 1, 95, 11523, STD, 401, 390, 23, 130, 3, "Remove Week", "Remove the currently highlighted week schedule from the list"


   ;*****************************************
   ; Week Schedules Page
   ;*****************************************
   TABPAGE, 3159, 32002, 1, 3, WEEK-SCHEDULE, " Week Schedules "

   COMBO, 15125, 0, 0, 1, WEEK-SCHEDULE, 0, NAME,  0, STD, 240,   5, 400, 250, 19, 3, "Currently Active Week Schedule:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all week schedules defined in project; also allows library retrieval and creation"
   STATIC, 1, WEEK-SCHEDULE, 0, TYPE, 0, 0, 0, 510, 10, 175, STD, LEFT, "Type: ",   "", 0, 3

    LINE,  20, 40, 685, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

    EDIT, 15126,     0, 0, 1, WEEK-SCHEDULE, 0,          NAME,  0, STD, 155,  55,  23, 250, 32, 3,  "Week Schedule Name:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Name of week schedule; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 15127, 31540, 0, 1, WEEK-SCHEDULE, 0,          TYPE,  0, STD, 155,  80, 300, 250, 19, 3,                "Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
 
   LABEL, "Daily Schedule Assignments", STD, LEFT, 20, 125, 1, 0, 0, 405, 0, 3

; SAC 4/14/03 - Swapped order of HDD/CDD labels per MSA's request
; DEM 2/21/16 - Added weekend design day schdules
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 1
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 2
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 3
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 4
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 5
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 6
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 7
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 8
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 9
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 10
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  10, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 11
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  11, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 12
      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  0, STD, 185, 135, 250, 250, 19, 3, "                Monday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  1, STD, 185, 160, 250, 250, 19, 3, "               Tuesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  2, STD, 185, 185, 250, 250, 19, 3, "             Wednesday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  3, STD, 185, 210, 250, 250, 19, 3, "              Thursday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  4, STD, 185, 235, 250, 250, 19, 3, "                Friday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  5, STD, 185, 260, 250, 250, 19, 3, "              Saturday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  6, STD, 185, 285, 250, 250, 19, 3, "                Sunday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  7, STD, 185, 310, 250, 250, 19, 3, "              Holidays:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  8, STD, 185, 335, 250, 250, 19, 3, "Heating Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES,  9, STD, 185, 360, 250, 250, 19, 3, "Cooling Des Day, Wkday:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19338,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES, 10, STD, 185, 385, 250, 250, 19, 3, "Heating Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
      COMBO, 19339,  1838, 0, 1, WEEK-SCHEDULE,  12, DAY-SCHEDULES, 11, STD, 185, 410, 250, 250, 19, 3, "Cooling Des Day, Wkend:",  RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
    ENDCASE     

   ;*****************************************
   ; Day Schedules Page
   ;*****************************************
   TABPAGE, 3161, 32003, 1, 3, DAY-SCHEDULE, " Day Schedules "

   COMBO, 15138, 0, 0, 1, DAY-SCHEDULE, 0, NAME,  0, STD, 240,   5, 400, 250, 19, 3, "Currently Active Day Schedule:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "List of all day schedules defined in project; also allows library retrieval and creation"
   STATIC, 1, DAY-SCHEDULE, 0, TYPE, 0, 0, 0, 510, 10, 175, STD, LEFT, "Type: ",   "", 0, 3

    LINE,  20, 40, 685, 40, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3

    EDIT, 15139,     0, 0, 1, DAY-SCHEDULE, 0,          NAME,  0, STD, 150,  55,  23, 250, 32, 3,  "Day Schedule Name:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Name of day schedule; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 15140, 31540, 0, 1, DAY-SCHEDULE, 0,          TYPE,  0, STD, 150,  80, 300, 250, 19, 3,               "Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "The type of day schedule (must be the same as parent week and annual schedules)"
 
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  1
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  1, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  1, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  0, STD,  95, 145,  23,  75,  0, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  1, STD,  95, 170,  23,  75,  0, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  2, STD,  95, 195,  23,  75,  0, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  3, STD,  95, 220,  23,  75,  0, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  4, STD,  95, 245,  23,  75,  0, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  5, STD,  95, 270,  23,  75,  0, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  6, STD,  95, 295,  23,  75,  0, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  7, STD,  95, 320,  23,  75,  0, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  8, STD, 330, 145,  23,  75,  0, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  9, STD, 330, 170,  23,  75,  0, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 10, STD, 330, 195,  23,  75,  0, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 11, STD, 330, 220,  23,  75,  0, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 12, STD, 330, 245,  23,  75,  0, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 13, STD, 330, 270,  23,  75,  0, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 14, STD, 330, 295,  23,  75,  0, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 15, STD, 330, 320,  23,  75,  0, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 16, STD, 565, 145,  23,  75,  0, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 17, STD, 565, 170,  23,  75,  0, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 18, STD, 565, 195,  23,  75,  0, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 19, STD, 565, 220,  23,  75,  0, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 20, STD, 565, 245,  23,  75,  0, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 21, STD, 565, 270,  23,  75,  0, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 22, STD, 565, 295,  23,  75,  0, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 23, STD, 565, 320,  23,  75,  0, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  2
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  2, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  2, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  0, STD,  95, 145,  23,  75,  4, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  1, STD,  95, 170,  23,  75,  4, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  2, STD,  95, 195,  23,  75,  4, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  3, STD,  95, 220,  23,  75,  4, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  4, STD,  95, 245,  23,  75,  4, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  5, STD,  95, 270,  23,  75,  4, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  6, STD,  95, 295,  23,  75,  4, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  7, STD,  95, 320,  23,  75,  4, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  8, STD, 330, 145,  23,  75,  4, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  9, STD, 330, 170,  23,  75,  4, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 10, STD, 330, 195,  23,  75,  4, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 11, STD, 330, 220,  23,  75,  4, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 12, STD, 330, 245,  23,  75,  4, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 13, STD, 330, 270,  23,  75,  4, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 14, STD, 330, 295,  23,  75,  4, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 15, STD, 330, 320,  23,  75,  4, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 16, STD, 565, 145,  23,  75,  4, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 17, STD, 565, 170,  23,  75,  4, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 18, STD, 565, 195,  23,  75,  4, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 19, STD, 565, 220,  23,  75,  4, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 20, STD, 565, 245,  23,  75,  4, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 21, STD, 565, 270,  23,  75,  4, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 22, STD, 565, 295,  23,  75,  4, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 23, STD, 565, 320,  23,  75,  4, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  3
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  3, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  3, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  0, STD,  95, 145,  23,  75,  4, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  1, STD,  95, 170,  23,  75,  4, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  2, STD,  95, 195,  23,  75,  4, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  3, STD,  95, 220,  23,  75,  4, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  4, STD,  95, 245,  23,  75,  4, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  5, STD,  95, 270,  23,  75,  4, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  6, STD,  95, 295,  23,  75,  4, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  7, STD,  95, 320,  23,  75,  4, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  8, STD, 330, 145,  23,  75,  4, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  9, STD, 330, 170,  23,  75,  4, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 10, STD, 330, 195,  23,  75,  4, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 11, STD, 330, 220,  23,  75,  4, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 12, STD, 330, 245,  23,  75,  4, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 13, STD, 330, 270,  23,  75,  4, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 14, STD, 330, 295,  23,  75,  4, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 15, STD, 330, 320,  23,  75,  4, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 16, STD, 565, 145,  23,  75,  4, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 17, STD, 565, 170,  23,  75,  4, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 18, STD, 565, 195,  23,  75,  4, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 19, STD, 565, 220,  23,  75,  4, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 20, STD, 565, 245,  23,  75,  4, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 21, STD, 565, 270,  23,  75,  4, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 22, STD, 565, 295,  23,  75,  4, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 23, STD, 565, 320,  23,  75,  4, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  4
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  4, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  4, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  0, STD,  95, 145,  23,  75,  1, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  1, STD,  95, 170,  23,  75,  1, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  2, STD,  95, 195,  23,  75,  1, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  3, STD,  95, 220,  23,  75,  1, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  4, STD,  95, 245,  23,  75,  1, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  5, STD,  95, 270,  23,  75,  1, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  6, STD,  95, 295,  23,  75,  1, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  7, STD,  95, 320,  23,  75,  1, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  8, STD, 330, 145,  23,  75,  1, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  9, STD, 330, 170,  23,  75,  1, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 10, STD, 330, 195,  23,  75,  1, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 11, STD, 330, 220,  23,  75,  1, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 12, STD, 330, 245,  23,  75,  1, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 13, STD, 330, 270,  23,  75,  1, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 14, STD, 330, 295,  23,  75,  1, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 15, STD, 330, 320,  23,  75,  1, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 16, STD, 565, 145,  23,  75,  1, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 17, STD, 565, 170,  23,  75,  1, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 18, STD, 565, 195,  23,  75,  1, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 19, STD, 565, 220,  23,  75,  1, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 20, STD, 565, 245,  23,  75,  1, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 21, STD, 565, 270,  23,  75,  1, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 22, STD, 565, 295,  23,  75,  1, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 23, STD, 565, 320,  23,  75,  1, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  5
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  5, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  5, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  0, STD,  95, 145,  23,  75,  1, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  1, STD,  95, 170,  23,  75,  1, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  2, STD,  95, 195,  23,  75,  1, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  3, STD,  95, 220,  23,  75,  1, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  4, STD,  95, 245,  23,  75,  1, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  5, STD,  95, 270,  23,  75,  1, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  6, STD,  95, 295,  23,  75,  1, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  7, STD,  95, 320,  23,  75,  1, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  8, STD, 330, 145,  23,  75,  1, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  9, STD, 330, 170,  23,  75,  1, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 10, STD, 330, 195,  23,  75,  1, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 11, STD, 330, 220,  23,  75,  1, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 12, STD, 330, 245,  23,  75,  1, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 13, STD, 330, 270,  23,  75,  1, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 14, STD, 330, 295,  23,  75,  1, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 15, STD, 330, 320,  23,  75,  1, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 16, STD, 565, 145,  23,  75,  1, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 17, STD, 565, 170,  23,  75,  1, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 18, STD, 565, 195,  23,  75,  1, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 19, STD, 565, 220,  23,  75,  1, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 20, STD, 565, 245,  23,  75,  1, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 21, STD, 565, 270,  23,  75,  1, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 22, STD, 565, 295,  23,  75,  1, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 23, STD, 565, 320,  23,  75,  1, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  6
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  6, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  6, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  0, STD,  95, 145,  23,  75,  0, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  1, STD,  95, 170,  23,  75,  0, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  2, STD,  95, 195,  23,  75,  0, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  3, STD,  95, 220,  23,  75,  0, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  4, STD,  95, 245,  23,  75,  0, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  5, STD,  95, 270,  23,  75,  0, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  6, STD,  95, 295,  23,  75,  0, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  7, STD,  95, 320,  23,  75,  0, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  8, STD, 330, 145,  23,  75,  0, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  9, STD, 330, 170,  23,  75,  0, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 10, STD, 330, 195,  23,  75,  0, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 11, STD, 330, 220,  23,  75,  0, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 12, STD, 330, 245,  23,  75,  0, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 13, STD, 330, 270,  23,  75,  0, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 14, STD, 330, 295,  23,  75,  0, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 15, STD, 330, 320,  23,  75,  0, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 16, STD, 565, 145,  23,  75,  0, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 17, STD, 565, 170,  23,  75,  0, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 18, STD, 565, 195,  23,  75,  0, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 19, STD, 565, 220,  23,  75,  0, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 20, STD, 565, 245,  23,  75,  0, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 21, STD, 565, 270,  23,  75,  0, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 22, STD, 565, 295,  23,  75,  0, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 23, STD, 565, 320,  23,  75,  0, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  7
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  7, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  7, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  0, STD,  95, 145,  23,  75,  0, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  1, STD,  95, 170,  23,  75,  0, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  2, STD,  95, 195,  23,  75,  0, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  3, STD,  95, 220,  23,  75,  0, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  4, STD,  95, 245,  23,  75,  0, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  5, STD,  95, 270,  23,  75,  0, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  6, STD,  95, 295,  23,  75,  0, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  7, STD,  95, 320,  23,  75,  0, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  8, STD, 330, 145,  23,  75,  0, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  9, STD, 330, 170,  23,  75,  0, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 10, STD, 330, 195,  23,  75,  0, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 11, STD, 330, 220,  23,  75,  0, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 12, STD, 330, 245,  23,  75,  0, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 13, STD, 330, 270,  23,  75,  0, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 14, STD, 330, 295,  23,  75,  0, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 15, STD, 330, 320,  23,  75,  0, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 16, STD, 565, 145,  23,  75,  0, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 17, STD, 565, 170,  23,  75,  0, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 18, STD, 565, 195,  23,  75,  0, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 19, STD, 565, 220,  23,  75,  0, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 20, STD, 565, 245,  23,  75,  0, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 21, STD, 565, 270,  23,  75,  0, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 22, STD, 565, 295,  23,  75,  0, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 23, STD, 565, 320,  23,  75,  0, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  8
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  8, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  8, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  0, STD,  95, 145,  23,  75,  4, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  1, STD,  95, 170,  23,  75,  4, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  2, STD,  95, 195,  23,  75,  4, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  3, STD,  95, 220,  23,  75,  4, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  4, STD,  95, 245,  23,  75,  4, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  5, STD,  95, 270,  23,  75,  4, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  6, STD,  95, 295,  23,  75,  4, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  7, STD,  95, 320,  23,  75,  4, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  8, STD, 330, 145,  23,  75,  4, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  9, STD, 330, 170,  23,  75,  4, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 10, STD, 330, 195,  23,  75,  4, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 11, STD, 330, 220,  23,  75,  4, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 12, STD, 330, 245,  23,  75,  4, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 13, STD, 330, 270,  23,  75,  4, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 14, STD, 330, 295,  23,  75,  4, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 15, STD, 330, 320,  23,  75,  4, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 16, STD, 565, 145,  23,  75,  4, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 17, STD, 565, 170,  23,  75,  4, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 18, STD, 565, 195,  23,  75,  4, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 19, STD, 565, 220,  23,  75,  4, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 20, STD, 565, 245,  23,  75,  4, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 21, STD, 565, 270,  23,  75,  4, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 22, STD, 565, 295,  23,  75,  4, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 23, STD, 565, 320,  23,  75,  4, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  9
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  9, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  9, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  0, STD,  95, 145,  23,  75,  4, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  1, STD,  95, 170,  23,  75,  4, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  2, STD,  95, 195,  23,  75,  4, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  3, STD,  95, 220,  23,  75,  4, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  4, STD,  95, 245,  23,  75,  4, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  5, STD,  95, 270,  23,  75,  4, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  6, STD,  95, 295,  23,  75,  4, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  7, STD,  95, 320,  23,  75,  4, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  8, STD, 330, 145,  23,  75,  4, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  9, STD, 330, 170,  23,  75,  4, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 10, STD, 330, 195,  23,  75,  4, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 11, STD, 330, 220,  23,  75,  4, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 12, STD, 330, 245,  23,  75,  4, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 13, STD, 330, 270,  23,  75,  4, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 14, STD, 330, 295,  23,  75,  4, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 15, STD, 330, 320,  23,  75,  4, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 16, STD, 565, 145,  23,  75,  4, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 17, STD, 565, 170,  23,  75,  4, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 18, STD, 565, 195,  23,  75,  4, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 19, STD, 565, 220,  23,  75,  4, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 20, STD, 565, 245,  23,  75,  4, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 21, STD, 565, 270,  23,  75,  4, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 22, STD, 565, 295,  23,  75,  4, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 23, STD, 565, 320,  23,  75,  4, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1, 10
;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE, 10, SCALE,   0, STD, 600,  10,  23,  60,  2, 3,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE, 10, BIAS,    0, STD, 600,  35,  23,  60,  2, 3,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
      LABEL, "Hourly Values", STD, LEFT, 20, 125, 1, 0, 0, 685, 15141, 3
       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  0, STD,  95, 145,  23,  75,  1, 3,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  1, STD,  95, 170,  23,  75,  1, 3,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  2, STD,  95, 195,  23,  75,  1, 3,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  3, STD,  95, 220,  23,  75,  1, 3,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  4, STD,  95, 245,  23,  75,  1, 3,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  5, STD,  95, 270,  23,  75,  1, 3,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  6, STD,  95, 295,  23,  75,  1, 3,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  7, STD,  95, 320,  23,  75,  1, 3,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  8, STD, 330, 145,  23,  75,  1, 3,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  9, STD, 330, 170,  23,  75,  1, 3,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 10, STD, 330, 195,  23,  75,  1, 3,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 11, STD, 330, 220,  23,  75,  1, 3,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 12, STD, 330, 245,  23,  75,  1, 3,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 13, STD, 330, 270,  23,  75,  1, 3,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 14, STD, 330, 295,  23,  75,  1, 3,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 15, STD, 330, 320,  23,  75,  1, 3,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""

       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 16, STD, 565, 145,  23,  75,  1, 3,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 17, STD, 565, 170,  23,  75,  1, 3,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 18, STD, 565, 195,  23,  75,  1, 3,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 19, STD, 565, 220,  23,  75,  1, 3,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 20, STD, 565, 245,  23,  75,  1, 3,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 21, STD, 565, 270,  23,  75,  1, 3,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 22, STD, 565, 295,  23,  75,  1, 3,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 23, STD, 565, 320,  23,  75,  1, 3,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1, 11
      LABEL, "Primary Reset Schedule", STD, LEFT, 20, 133, 1, 0, 0, 325, 15141, 3
      LABEL, "First Hr", STD, CENTER, 232, 149, 1, 0, 0, 0, 15141, 3
      LABEL, "Last Hr",  STD, CENTER, 285, 149, 1, 0, 0, 0, 15141, 3
       EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE, 11, DAY-HOURS,    0, STD, 212, 165,  23,  40,  0, 3,                "Primary Reset Hours:",  LEFT, -180, 5, 0, LEFT, 4, 5, "The first hour of the day for which the Primary reset parameters are used"
       EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE, 11, DAY-HOURS,    1, STD, 265, 165,  23,  40,  0, 3,                                   "-", RIGHT,   -4, 5, 0, LEFT, 4, 5, "The last hour of the day for which the Primary reset parameters are used"

       EDIT, 15143, 31541, 0, 1, DAY-SCHEDULE, 11, OUTSIDE-HI,   0, STD, 255, 190,  23,  50,  1, 3,   "Outdoor DryBulb High Temperature:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the lower supply air set-point temperature"
       EDIT, 15144, 31541, 0, 1, DAY-SCHEDULE, 11, OUTSIDE-LO,   0, STD, 255, 215,  23,  50,  1, 3,    "Outdoor DryBulb Low Temperature:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the upper supply air set-point temperature"
       EDIT, 15145, 31544, 0, 1, DAY-SCHEDULE, 11, SUPPLY-HI,    0, STD, 255, 240,  23,  50,  1, 3,  "Supply Leaving Temp @ Outdoor Low:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The upper supply air set-point temp that corresponds to the Outside Drybulb Temp Low"
       EDIT, 15146, 31544, 0, 1, DAY-SCHEDULE, 11, SUPPLY-LO,    0, STD, 255, 265,  23,  50,  1, 3, "Supply Leaving Temp @ Outdoor High:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The lower supply air set-point temp that corresponds to the Outside Drybulb Temp High"

      LABEL, "Alternate Reset Schedule",          STD, LEFT, 375, 150, 1, 0, 0, 690, 15147, 3
      LABEL, "(applies to all remaining hours)",  STD, LEFT, 385, 170, 1, 0, 0,   0, 15147, 3
       EDIT, 15147, 31541, 0, 1, DAY-SCHEDULE, 11, OUTSIDE-HI2,  0, STD, 610, 190,  23,  50,  1, 3,   "Outdoor DryBulb High Temperature:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the lower supply air set-point temperature"
       EDIT, 15148, 31541, 0, 1, DAY-SCHEDULE, 11, OUTSIDE-LO2,  0, STD, 610, 215,  23,  50,  1, 3,    "Outdoor DryBulb Low Temperature:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the upper supply air set-point temperature"
       EDIT, 15149, 31544, 0, 1, DAY-SCHEDULE, 11, SUPPLY-HI2,   0, STD, 610, 240,  23,  50,  1, 3,  "Supply Leaving Temp @ Outdoor Low:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The upper supply air set-point temp that corresponds to the Outside Drybulb Temp Low"
       EDIT, 15150, 31544, 0, 1, DAY-SCHEDULE, 11, SUPPLY-LO2,   0, STD, 610, 265,  23,  50,  1, 3, "Supply Leaving Temp @ Outdoor High:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The lower supply air set-point temp that corresponds to the Outside Drybulb Temp High"
    ENDCASE     
    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1, 12
      LABEL, "Primary Reset Schedule", STD, LEFT, 20, 133, 1, 0, 0, 325, 15141, 3
      LABEL, "First Hr", STD, CENTER, 232, 149, 1, 0, 0, 0, 15141, 3
      LABEL, "Last Hr",  STD, CENTER, 285, 149, 1, 0, 0, 0, 15141, 3
       EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE, 12, DAY-HOURS,    0, STD, 212, 165,  23,  40,  0, 3,                  "Primary Reset Hours:",  LEFT, -180, 5, 0, LEFT, 4, 5, "The first hour of the day for which the Primary reset parameters are used"
       EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE, 12, DAY-HOURS,    1, STD, 265, 165,  23,  40,  0, 3,                                     "-", RIGHT,   -4, 5, 0, LEFT, 4, 5, "The last hour of the day for which the Primary reset parameters are used"

       EDIT, 15143, 31541, 0, 1, DAY-SCHEDULE, 12, OUTSIDE-HI,   0, STD, 255, 190,  23,  50,  1, 3,        "Outdoor DryBulb High Setpoint:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the lower supply air set-point temperature"
       EDIT, 15144, 31541, 0, 1, DAY-SCHEDULE, 12, OUTSIDE-LO,   0, STD, 255, 215,  23,  50,  1, 3,         "Outdoor DryBulb Low Setpoint:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the upper supply air set-point temperature"
       EDIT, 15145, 31544, 0, 1, DAY-SCHEDULE, 12, SUPPLY-HI,    0, STD, 255, 240,  23,  50,  2, 3,  "Supply Capacity Ratio @ Outdoor Low:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The upper supply air set-point temp that corresponds to the Outside Drybulb Temp Low"
       EDIT, 15146, 31544, 0, 1, DAY-SCHEDULE, 12, SUPPLY-LO,    0, STD, 255, 265,  23,  50,  2, 3, "Supply Capacity Ratio @ Outdoor High:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The lower supply air set-point temp that corresponds to the Outside Drybulb Temp High"

      LABEL, "Alternate Reset Schedule",          STD, LEFT, 375, 150, 1, 0, 0, 690, 15147, 3
      LABEL, "(applies to all remaining hours)",  STD, LEFT, 385, 170, 1, 0, 0,   0, 15147, 3
       EDIT, 15147, 31541, 0, 1, DAY-SCHEDULE, 12, OUTSIDE-HI2,  0, STD, 610, 190,  23,  50,  1, 3,        "Outdoor DryBulb High Setpoint:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the lower supply air set-point temperature"
       EDIT, 15148, 31541, 0, 1, DAY-SCHEDULE, 12, OUTSIDE-LO2,  0, STD, 610, 215,  23,  50,  1, 3,         "Outdoor DryBulb Low Setpoint:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the upper supply air set-point temperature"
       EDIT, 15149, 31544, 0, 1, DAY-SCHEDULE, 12, SUPPLY-HI2,   0, STD, 610, 240,  23,  50,  2, 3,  "Supply Capacity Ratio @ Outdoor Low:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The upper supply air set-point temp that corresponds to the Outside Drybulb Temp Low"
       EDIT, 15150, 31544, 0, 1, DAY-SCHEDULE, 12, SUPPLY-LO2,   0, STD, 610, 265,  23,  50,  2, 3, "Supply Capacity Ratio @ Outdoor High:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The lower supply air set-point temp that corresponds to the Outside Drybulb Temp High"
    ENDCASE     



;  vvvvv  OLD VERSIONS OF SCHEDULE DIALOGS AS SEPARATE TABBED DIALOGS  vvvvv
;  vvvvv  OLD VERSIONS OF SCHEDULE DIALOGS AS SEPARATE TABBED DIALOGS  vvvvv

; ;********************************************************************
; ;********************************************************************
; ;**
; ;**     Schedule Tabbed Dialog
; ;**
; ;********************************************************************
; ;********************************************************************
;MODTABDLG, 3156, 32001, 1, 100, 100, 470, 710, 0, SCHEDULE, "Schedule Properties", NOTIMP, 0, NOTIMP, 0
; 
;   COMBO, 15121, 0, 0, 1, SCHEDULE, 0, NAME,  0, STD, 180,  15, 400, 250, 19, "Currently Active Schedule:",  LEFT, -165, 5, 0, LEFT, 4, 5, "List of all schedules defined in project; also allows library retrieval and creation"
;   STATIC, 1, SCHEDULE, 0, TYPE, 0, 0, 0, 450, 20, 250, STD, LEFT, "Type: ",   "", 0
;
;   ;*****************************************
;   ; Basic Specifications 
;   ;*****************************************
;   TABPAGE, 3157, 32001, 1, 3, NOTIMP, " Basic Specifications "
;
;    EDIT, 15122,     0, 0, 1, SCHEDULE, 0,             NAME,  0, STD, 125,  10,  23, 250, 32,     "Schedule Name:",  LEFT, -105, 5, 1, LEFT, 4, 5, "Name of schedule; right mouse quick menu options allow deleting, copying, linking and saving to library"
;   COMBO, 15123, 31540, 0, 1, SCHEDULE, 0,             TYPE,  0, STD, 125,  35, 250, 250, 19,              "Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
;   COMBO, 15124,     0, 0, 1, SCHEDULE, 0,            GROUP,  0, STD, 125,  60, 120, 250, 19,             "Group:", RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
;
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 1
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread1,  0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 2
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread2,  0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 3
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread3,  0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 4
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread4,  0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 5
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread5,  0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 6
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread6,  0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 7
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread7,  0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 8
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread8,  0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 9
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread9,  0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 10
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread10, 0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  SCHEDULE,  0, TYPE,  -1,  =, 1, 11
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread11, 0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;    CASE,  ELSE
;       SPREAD, 11523, 11523, 0, 1, 0, PowerDOE, 0,  AnnSchSpread12, 0, STD, 125, 107, 260, 406, 19, "Weekly Schedule Assignments:",  LEFT, -50, -17, 0, LEFT, 0, 0, ""
;    ENDCASE     
;
;
;
; ;********************************************************************
; ;********************************************************************
; ;**
; ;**     Week Schedule Tabbed Dialog
; ;**
; ;********************************************************************
; ;********************************************************************
;MODTABDLG, 3158, 32002, 1, 100, 100, 470, 710, 0, WEEK-SCHEDULE, "Week Schedule Properties", NOTIMP, 0, NOTIMP, 0
; 
;   COMBO, 15125, 0, 0, 1, WEEK-SCHEDULE, 0, NAME,  0, STD, 210,  15, 400, 250, 19, "Currently Active Week Schedule:",  LEFT, -195, 5, 0, LEFT, 4, 5, "List of all week schedules defined in project; also allows library retrieval and creation"
;   STATIC, 1, WEEK-SCHEDULE, 0, TYPE, 0, 0, 0, 480, 20, 250, STD, LEFT, "Type: ",   "", 0
;
;   ;*****************************************
;   ; Basic Specifications 
;   ;*****************************************
;   TABPAGE, 3159, 32002, 1, 3, NOTIMP, " Basic Specifications "
;
;    EDIT, 15126,     0, 0, 1, WEEK-SCHEDULE, 0,          NAME,  0, STD, 155,  10,  23, 250, 32,  "Week Schedule Name:",  LEFT, -135, 5, 1, LEFT, 4, 5, "Name of week schedule; right mouse quick menu options allow deleting, copying, linking and saving to library"
;   COMBO, 15127, 31540, 0, 1, WEEK-SCHEDULE, 0,          TYPE,  0, STD, 155,  35, 250, 250, 19,                "Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, ""
; 
;   LABEL, "Daily Schedule Assignments", STD, LEFT, 20, 80, 1, 0, 0, 405, 0, 3
;
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 1
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  1, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 2
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  2, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 3
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  3, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 4
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  4, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 5
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  5, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 6
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  6, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 7
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  7, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 8
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  8, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 9
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE,  9, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 10
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE, 10, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 11
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE, 11, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  WEEK-SCHEDULE,  0, TYPE,  -1,  =, 1, 12
;      COMBO, 15128,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  0, STD, 155, 100, 250, 250, 19,             "Monday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15129,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  1, STD, 155, 125, 250, 250, 19,            "Tuesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15130,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  2, STD, 155, 150, 250, 250, 19,          "Wednesday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15131,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  3, STD, 155, 175, 250, 250, 19,           "Thursday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15132,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  4, STD, 155, 200, 250, 250, 19,             "Friday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15133,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  5, STD, 155, 225, 250, 250, 19,           "Saturday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15134,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  6, STD, 155, 250, 250, 250, 19,             "Sunday:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15135,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  7, STD, 155, 275, 250, 250, 19,           "Holidays:",  LEFT,  -95, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15136,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  8, STD, 155, 300, 250, 250, 19, "Heating Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;      COMBO, 15137,  1838, 0, 1, WEEK-SCHEDULE, 12, DAY-SCHEDULES,  9, STD, 155, 325, 250, 250, 19, "Cooling Design Day:",  LEFT, -125, 5, 0, LEFT, 4, 5, ""
;    ENDCASE     
;
;
;
; ;********************************************************************
; ;********************************************************************
; ;**
; ;**     Day Schedule Tabbed Dialog
; ;**
; ;********************************************************************
; ;********************************************************************
;MODTABDLG, 3160, 32003, 1, 100, 100, 470, 710, 0, DAY-SCHEDULE, "Day Schedule Properties", NOTIMP, 0, NOTIMP, 0
; 
;   COMBO, 15138, 0, 0, 1, DAY-SCHEDULE, 0, NAME,  0, STD, 205,  15, 400, 250, 19, "Currently Active Day Schedule:",  LEFT, -190, 5, 0, LEFT, 4, 5, "List of all day schedules defined in project; also allows library retrieval and creation"
;   STATIC, 1, DAY-SCHEDULE, 0, TYPE, 0, 0, 0, 475, 20, 250, STD, LEFT, "Type: ",   "", 0
;
;   ;*****************************************
;   ; Basic Specifications 
;   ;*****************************************
;   TABPAGE, 3161, 32003, 1, 3, NOTIMP, " Basic Specifications "
;
;    EDIT, 15139,     0, 0, 1, DAY-SCHEDULE, 0,          NAME,  0, STD, 150,  10,  23, 250, 32,  "Day Schedule Name:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Name of day schedule; right mouse quick menu options allow deleting, copying, linking and saving to library"
;   COMBO, 15140, 31540, 0, 1, DAY-SCHEDULE, 0,          TYPE,  0, STD, 150,  35, 250, 250, 19,               "Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "The type of day schedule (must be the same as parent week and annual schedules)"
; 
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  1
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  1, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  1, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  0, STD,  95, 100,  23,  75,  0,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  1, STD,  95, 125,  23,  75,  0,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  2, STD,  95, 150,  23,  75,  0,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  3, STD,  95, 175,  23,  75,  0,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  4, STD,  95, 200,  23,  75,  0,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  5, STD,  95, 225,  23,  75,  0,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  6, STD,  95, 250,  23,  75,  0,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  7, STD,  95, 275,  23,  75,  0,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  8, STD, 330, 100,  23,  75,  0,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES,  9, STD, 330, 125,  23,  75,  0,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 10, STD, 330, 150,  23,  75,  0,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 11, STD, 330, 175,  23,  75,  0,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 12, STD, 330, 200,  23,  75,  0,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 13, STD, 330, 225,  23,  75,  0,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 14, STD, 330, 250,  23,  75,  0,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 15, STD, 330, 275,  23,  75,  0,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 16, STD, 565, 100,  23,  75,  0,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 17, STD, 565, 125,  23,  75,  0,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 18, STD, 565, 150,  23,  75,  0,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 19, STD, 565, 175,  23,  75,  0,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 20, STD, 565, 200,  23,  75,  0,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 21, STD, 565, 225,  23,  75,  0,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 22, STD, 565, 250,  23,  75,  0,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  1, VALUES, 23, STD, 565, 275,  23,  75,  0,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  2
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  2, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  2, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  0, STD,  95, 100,  23,  75,  4,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  1, STD,  95, 125,  23,  75,  4,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  2, STD,  95, 150,  23,  75,  4,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  3, STD,  95, 175,  23,  75,  4,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  4, STD,  95, 200,  23,  75,  4,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  5, STD,  95, 225,  23,  75,  4,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  6, STD,  95, 250,  23,  75,  4,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  7, STD,  95, 275,  23,  75,  4,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  8, STD, 330, 100,  23,  75,  4,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES,  9, STD, 330, 125,  23,  75,  4,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 10, STD, 330, 150,  23,  75,  4,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 11, STD, 330, 175,  23,  75,  4,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 12, STD, 330, 200,  23,  75,  4,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 13, STD, 330, 225,  23,  75,  4,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 14, STD, 330, 250,  23,  75,  4,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 15, STD, 330, 275,  23,  75,  4,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 16, STD, 565, 100,  23,  75,  4,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 17, STD, 565, 125,  23,  75,  4,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 18, STD, 565, 150,  23,  75,  4,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 19, STD, 565, 175,  23,  75,  4,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 20, STD, 565, 200,  23,  75,  4,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 21, STD, 565, 225,  23,  75,  4,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 22, STD, 565, 250,  23,  75,  4,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  2, VALUES, 23, STD, 565, 275,  23,  75,  4,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  3
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  3, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  3, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  0, STD,  95, 100,  23,  75,  4,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  1, STD,  95, 125,  23,  75,  4,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  2, STD,  95, 150,  23,  75,  4,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  3, STD,  95, 175,  23,  75,  4,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  4, STD,  95, 200,  23,  75,  4,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  5, STD,  95, 225,  23,  75,  4,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  6, STD,  95, 250,  23,  75,  4,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  7, STD,  95, 275,  23,  75,  4,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  8, STD, 330, 100,  23,  75,  4,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES,  9, STD, 330, 125,  23,  75,  4,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 10, STD, 330, 150,  23,  75,  4,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 11, STD, 330, 175,  23,  75,  4,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 12, STD, 330, 200,  23,  75,  4,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 13, STD, 330, 225,  23,  75,  4,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 14, STD, 330, 250,  23,  75,  4,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 15, STD, 330, 275,  23,  75,  4,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 16, STD, 565, 100,  23,  75,  4,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 17, STD, 565, 125,  23,  75,  4,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 18, STD, 565, 150,  23,  75,  4,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 19, STD, 565, 175,  23,  75,  4,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 20, STD, 565, 200,  23,  75,  4,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 21, STD, 565, 225,  23,  75,  4,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 22, STD, 565, 250,  23,  75,  4,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  3, VALUES, 23, STD, 565, 275,  23,  75,  4,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  4
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  4, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  4, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  0, STD,  95, 100,  23,  75,  1,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  1, STD,  95, 125,  23,  75,  1,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  2, STD,  95, 150,  23,  75,  1,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  3, STD,  95, 175,  23,  75,  1,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  4, STD,  95, 200,  23,  75,  1,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  5, STD,  95, 225,  23,  75,  1,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  6, STD,  95, 250,  23,  75,  1,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  7, STD,  95, 275,  23,  75,  1,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  8, STD, 330, 100,  23,  75,  1,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES,  9, STD, 330, 125,  23,  75,  1,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 10, STD, 330, 150,  23,  75,  1,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 11, STD, 330, 175,  23,  75,  1,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 12, STD, 330, 200,  23,  75,  1,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 13, STD, 330, 225,  23,  75,  1,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 14, STD, 330, 250,  23,  75,  1,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 15, STD, 330, 275,  23,  75,  1,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 16, STD, 565, 100,  23,  75,  1,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 17, STD, 565, 125,  23,  75,  1,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 18, STD, 565, 150,  23,  75,  1,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 19, STD, 565, 175,  23,  75,  1,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 20, STD, 565, 200,  23,  75,  1,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 21, STD, 565, 225,  23,  75,  1,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 22, STD, 565, 250,  23,  75,  1,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  4, VALUES, 23, STD, 565, 275,  23,  75,  1,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  5
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  5, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  5, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  0, STD,  95, 100,  23,  75,  1,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  1, STD,  95, 125,  23,  75,  1,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  2, STD,  95, 150,  23,  75,  1,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  3, STD,  95, 175,  23,  75,  1,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  4, STD,  95, 200,  23,  75,  1,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  5, STD,  95, 225,  23,  75,  1,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  6, STD,  95, 250,  23,  75,  1,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  7, STD,  95, 275,  23,  75,  1,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  8, STD, 330, 100,  23,  75,  1,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES,  9, STD, 330, 125,  23,  75,  1,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 10, STD, 330, 150,  23,  75,  1,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 11, STD, 330, 175,  23,  75,  1,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 12, STD, 330, 200,  23,  75,  1,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 13, STD, 330, 225,  23,  75,  1,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 14, STD, 330, 250,  23,  75,  1,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 15, STD, 330, 275,  23,  75,  1,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 16, STD, 565, 100,  23,  75,  1,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 17, STD, 565, 125,  23,  75,  1,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 18, STD, 565, 150,  23,  75,  1,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 19, STD, 565, 175,  23,  75,  1,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 20, STD, 565, 200,  23,  75,  1,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 21, STD, 565, 225,  23,  75,  1,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 22, STD, 565, 250,  23,  75,  1,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  5, VALUES, 23, STD, 565, 275,  23,  75,  1,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  6
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  6, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  6, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  0, STD,  95, 100,  23,  75,  0,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  1, STD,  95, 125,  23,  75,  0,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  2, STD,  95, 150,  23,  75,  0,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  3, STD,  95, 175,  23,  75,  0,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  4, STD,  95, 200,  23,  75,  0,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  5, STD,  95, 225,  23,  75,  0,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  6, STD,  95, 250,  23,  75,  0,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  7, STD,  95, 275,  23,  75,  0,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  8, STD, 330, 100,  23,  75,  0,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES,  9, STD, 330, 125,  23,  75,  0,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 10, STD, 330, 150,  23,  75,  0,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 11, STD, 330, 175,  23,  75,  0,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 12, STD, 330, 200,  23,  75,  0,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 13, STD, 330, 225,  23,  75,  0,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 14, STD, 330, 250,  23,  75,  0,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 15, STD, 330, 275,  23,  75,  0,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 16, STD, 565, 100,  23,  75,  0,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 17, STD, 565, 125,  23,  75,  0,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 18, STD, 565, 150,  23,  75,  0,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 19, STD, 565, 175,  23,  75,  0,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 20, STD, 565, 200,  23,  75,  0,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 21, STD, 565, 225,  23,  75,  0,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 22, STD, 565, 250,  23,  75,  0,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  6, VALUES, 23, STD, 565, 275,  23,  75,  0,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  7
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  7, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  7, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  0, STD,  95, 100,  23,  75,  0,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  1, STD,  95, 125,  23,  75,  0,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  2, STD,  95, 150,  23,  75,  0,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  3, STD,  95, 175,  23,  75,  0,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  4, STD,  95, 200,  23,  75,  0,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  5, STD,  95, 225,  23,  75,  0,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  6, STD,  95, 250,  23,  75,  0,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  7, STD,  95, 275,  23,  75,  0,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  8, STD, 330, 100,  23,  75,  0,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES,  9, STD, 330, 125,  23,  75,  0,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 10, STD, 330, 150,  23,  75,  0,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 11, STD, 330, 175,  23,  75,  0,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 12, STD, 330, 200,  23,  75,  0,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 13, STD, 330, 225,  23,  75,  0,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 14, STD, 330, 250,  23,  75,  0,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 15, STD, 330, 275,  23,  75,  0,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 16, STD, 565, 100,  23,  75,  0,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 17, STD, 565, 125,  23,  75,  0,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 18, STD, 565, 150,  23,  75,  0,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 19, STD, 565, 175,  23,  75,  0,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 20, STD, 565, 200,  23,  75,  0,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 21, STD, 565, 225,  23,  75,  0,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 22, STD, 565, 250,  23,  75,  0,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  7, VALUES, 23, STD, 565, 275,  23,  75,  0,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  8
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  8, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  8, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  0, STD,  95, 100,  23,  75,  4,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  1, STD,  95, 125,  23,  75,  4,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  2, STD,  95, 150,  23,  75,  4,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  3, STD,  95, 175,  23,  75,  4,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  4, STD,  95, 200,  23,  75,  4,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  5, STD,  95, 225,  23,  75,  4,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  6, STD,  95, 250,  23,  75,  4,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  7, STD,  95, 275,  23,  75,  4,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  8, STD, 330, 100,  23,  75,  4,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES,  9, STD, 330, 125,  23,  75,  4,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 10, STD, 330, 150,  23,  75,  4,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 11, STD, 330, 175,  23,  75,  4,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 12, STD, 330, 200,  23,  75,  4,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 13, STD, 330, 225,  23,  75,  4,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 14, STD, 330, 250,  23,  75,  4,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 15, STD, 330, 275,  23,  75,  4,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 16, STD, 565, 100,  23,  75,  4,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 17, STD, 565, 125,  23,  75,  4,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 18, STD, 565, 150,  23,  75,  4,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 19, STD, 565, 175,  23,  75,  4,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 20, STD, 565, 200,  23,  75,  4,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 21, STD, 565, 225,  23,  75,  4,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 22, STD, 565, 250,  23,  75,  4,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  8, VALUES, 23, STD, 565, 275,  23,  75,  4,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1,  9
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE,  9, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE,  9, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  0, STD,  95, 100,  23,  75,  4,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  1, STD,  95, 125,  23,  75,  4,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  2, STD,  95, 150,  23,  75,  4,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  3, STD,  95, 175,  23,  75,  4,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  4, STD,  95, 200,  23,  75,  4,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  5, STD,  95, 225,  23,  75,  4,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  6, STD,  95, 250,  23,  75,  4,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  7, STD,  95, 275,  23,  75,  4,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  8, STD, 330, 100,  23,  75,  4,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES,  9, STD, 330, 125,  23,  75,  4,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 10, STD, 330, 150,  23,  75,  4,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 11, STD, 330, 175,  23,  75,  4,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 12, STD, 330, 200,  23,  75,  4,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 13, STD, 330, 225,  23,  75,  4,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 14, STD, 330, 250,  23,  75,  4,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 15, STD, 330, 275,  23,  75,  4,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 16, STD, 565, 100,  23,  75,  4,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 17, STD, 565, 125,  23,  75,  4,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 18, STD, 565, 150,  23,  75,  4,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 19, STD, 565, 175,  23,  75,  4,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 20, STD, 565, 200,  23,  75,  4,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 21, STD, 565, 225,  23,  75,  4,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 22, STD, 565, 250,  23,  75,  4,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE,  9, VALUES, 23, STD, 565, 275,  23,  75,  4,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1, 10
;;      EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE, 10, SCALE,   0, STD, 600,  10,  23,  60,  2,         "Scale:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;;      EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE, 10, BIAS,    0, STD, 600,  35,  23,  60,  2,          "Bias:",  LEFT,  -50, 5, 1, LEFT, 4, 5, ""
;      LABEL, "Hourly Values", STD, LEFT, 20, 80, 1, 0, 0, 685, 15141, 3
;       EDIT, 15143, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  0, STD,  95, 100,  23,  75,  1,      "Mdnt - 1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15144, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  1, STD,  95, 125,  23,  75,  1,        "1-2 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15145, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  2, STD,  95, 150,  23,  75,  1,        "2-3 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15146, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  3, STD,  95, 175,  23,  75,  1,        "3-4 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15147, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  4, STD,  95, 200,  23,  75,  1,        "4-5 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15148, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  5, STD,  95, 225,  23,  75,  1,        "5-6 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15149, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  6, STD,  95, 250,  23,  75,  1,        "6-7 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15150, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  7, STD,  95, 275,  23,  75,  1,        "7-8 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15151, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  8, STD, 330, 100,  23,  75,  1,        "8-9 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15152, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES,  9, STD, 330, 125,  23,  75,  1,       "9-10 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15153, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 10, STD, 330, 150,  23,  75,  1,      "10-11 am:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15154, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 11, STD, 330, 175,  23,  75,  1,       "11-noon:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15155, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 12, STD, 330, 200,  23,  75,  1,        "noon-1:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15156, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 13, STD, 330, 225,  23,  75,  1,        "1-2 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15157, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 14, STD, 330, 250,  23,  75,  1,        "2-3 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15158, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 15, STD, 330, 275,  23,  75,  1,        "3-4 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;
;       EDIT, 15159, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 16, STD, 565, 100,  23,  75,  1,        "4-5 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15160, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 17, STD, 565, 125,  23,  75,  1,        "5-6 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15161, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 18, STD, 565, 150,  23,  75,  1,        "6-7 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15162, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 19, STD, 565, 175,  23,  75,  1,        "7-8 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15163, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 20, STD, 565, 200,  23,  75,  1,        "8-9 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15164, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 21, STD, 565, 225,  23,  75,  1,       "9-10 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15165, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 22, STD, 565, 250,  23,  75,  1,      "10-11 pm:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;       EDIT, 15166, 31570, 0, 1, DAY-SCHEDULE, 10, VALUES, 23, STD, 565, 275,  23,  75,  1,       "11-Mdnt:", RIGHT,   -7, 5, 1, LEFT, 4, 5, ""
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1, 11
;      LABEL, "Primary Reset Schedule", STD, LEFT, 20, 88, 1, 0, 0, 325, 15141, 3
;      LABEL, "First Hr", STD, CENTER, 232, 104, 1, 0, 0, 0, 15141, 3
;      LABEL, "Last Hr",  STD, CENTER, 285, 104, 1, 0, 0, 0, 15141, 3
;       EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE, 11, DAY-HOURS,    0, STD, 212, 120,  23,  40,  0,                "Primary Reset Hours:",  LEFT, -180, 5, 0, LEFT, 4, 5, "The first hour of the day for which the Primary reset parameters are used"
;       EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE, 11, DAY-HOURS,    1, STD, 265, 120,  23,  40,  0,                                   "-", RIGHT,   -4, 5, 0, LEFT, 4, 5, "The last hour of the day for which the Primary reset parameters are used"
;
;       EDIT, 15143, 31541, 0, 1, DAY-SCHEDULE, 11, OUTSIDE-HI,   0, STD, 255, 145,  23,  50,  1,   "Outdoor DryBulb High Temperature:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the lower supply air set-point temperature"
;       EDIT, 15144, 31541, 0, 1, DAY-SCHEDULE, 11, OUTSIDE-LO,   0, STD, 255, 170,  23,  50,  1,    "Outdoor DryBulb Low Temperature:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the upper supply air set-point temperature"
;       EDIT, 15145, 31544, 0, 1, DAY-SCHEDULE, 11, SUPPLY-HI,    0, STD, 255, 195,  23,  50,  1,  "Supply Leaving Temp @ Outdoor Low:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The upper supply air set-point temp that corresponds to the Outside Drybulb Temp Low"
;       EDIT, 15146, 31544, 0, 1, DAY-SCHEDULE, 11, SUPPLY-LO,    0, STD, 255, 220,  23,  50,  1, "Supply Leaving Temp @ Outdoor High:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The lower supply air set-point temp that corresponds to the Outside Drybulb Temp High"
;
;      LABEL, "Alternate Reset Schedule",  STD, LEFT, 375, 105, 1, 0, 0, 690, 15147, 3
;      LABEL, "(applies to all remaining hours)",  STD, LEFT, 385, 125, 1, 0, 0, 0, 15147, 3
;       EDIT, 15147, 31541, 0, 1, DAY-SCHEDULE, 11, OUTSIDE-HI2,  0, STD, 610, 145,  23,  50,  1,   "Outdoor DryBulb High Temperature:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the lower supply air set-point temperature"
;       EDIT, 15148, 31541, 0, 1, DAY-SCHEDULE, 11, OUTSIDE-LO2,  0, STD, 610, 170,  23,  50,  1,    "Outdoor DryBulb Low Temperature:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the upper supply air set-point temperature"
;       EDIT, 15149, 31544, 0, 1, DAY-SCHEDULE, 11, SUPPLY-HI2,   0, STD, 610, 195,  23,  50,  1,  "Supply Leaving Temp @ Outdoor Low:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The upper supply air set-point temp that corresponds to the Outside Drybulb Temp Low"
;       EDIT, 15150, 31544, 0, 1, DAY-SCHEDULE, 11, SUPPLY-LO2,   0, STD, 610, 220,  23,  50,  1, "Supply Leaving Temp @ Outdoor High:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The lower supply air set-point temp that corresponds to the Outside Drybulb Temp High"
;    ENDCASE     
;    CASE,  DAY-SCHEDULE,  0, TYPE,  -1,  =, 1, 12
;      LABEL, "Primary Reset Schedule", STD, LEFT, 20, 88, 1, 0, 0, 325, 15141, 3
;      LABEL, "First Hr", STD, CENTER, 232, 104, 1, 0, 0, 0, 15141, 3
;      LABEL, "Last Hr",  STD, CENTER, 285, 104, 1, 0, 0, 0, 15141, 3
;       EDIT, 15141, 31545, 0, 1, DAY-SCHEDULE, 12, DAY-HOURS,    0, STD, 212, 120,  23,  40,  0,                  "Primary Reset Hours:",  LEFT, -180, 5, 0, LEFT, 4, 5, "The first hour of the day for which the Primary reset parameters are used"
;       EDIT, 15142, 31545, 0, 1, DAY-SCHEDULE, 12, DAY-HOURS,    1, STD, 265, 120,  23,  40,  0,                                     "-", RIGHT,   -4, 5, 0, LEFT, 4, 5, "The last hour of the day for which the Primary reset parameters are used"
;
;       EDIT, 15143, 31541, 0, 1, DAY-SCHEDULE, 12, OUTSIDE-HI,   0, STD, 255, 145,  23,  50,  1,        "Outdoor DryBulb High Setpoint:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the lower supply air set-point temperature"
;       EDIT, 15144, 31541, 0, 1, DAY-SCHEDULE, 12, OUTSIDE-LO,   0, STD, 255, 170,  23,  50,  1,         "Outdoor DryBulb Low Setpoint:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the upper supply air set-point temperature"
;       EDIT, 15145, 31544, 0, 1, DAY-SCHEDULE, 12, SUPPLY-HI,    0, STD, 255, 195,  23,  50,  2,  "Supply Capacity Ratio @ Outdoor Low:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The upper supply air set-point temp that corresponds to the Outside Drybulb Temp Low"
;       EDIT, 15146, 31544, 0, 1, DAY-SCHEDULE, 12, SUPPLY-LO,    0, STD, 255, 220,  23,  50,  2, "Supply Capacity Ratio @ Outdoor High:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The lower supply air set-point temp that corresponds to the Outside Drybulb Temp High"
;
;      LABEL, "Alternate Reset Schedule",  STD, LEFT, 375, 105, 1, 0, 0, 690, 15147, 3
;      LABEL, "(applies to all remaining hours)",  STD, LEFT, 385, 125, 1, 0, 0, 0, 15147, 3
;       EDIT, 15147, 31541, 0, 1, DAY-SCHEDULE, 12, OUTSIDE-HI2,  0, STD, 610, 145,  23,  50,  1,        "Outdoor DryBulb High Setpoint:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the lower supply air set-point temperature"
;       EDIT, 15148, 31541, 0, 1, DAY-SCHEDULE, 12, OUTSIDE-LO2,  0, STD, 610, 170,  23,  50,  1,         "Outdoor DryBulb Low Setpoint:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The outside drybulb air temp that corresponds to the upper supply air set-point temperature"
;       EDIT, 15149, 31544, 0, 1, DAY-SCHEDULE, 12, SUPPLY-HI2,   0, STD, 610, 195,  23,  50,  2,  "Supply Capacity Ratio @ Outdoor Low:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The upper supply air set-point temp that corresponds to the Outside Drybulb Temp Low"
;       EDIT, 15150, 31544, 0, 1, DAY-SCHEDULE, 12, SUPPLY-LO2,   0, STD, 610, 220,  23,  50,  2, "Supply Capacity Ratio @ Outdoor High:",  LEFT, -225, 5, 1, LEFT, 4, 5, "The lower supply air set-point temp that corresponds to the Outside Drybulb Temp High"
;    ENDCASE     

;  ^^^^^  end of - OLD VERSIONS OF SCHEDULE DIALOGS AS SEPARATE TABBED DIALOGS  ^^^^^
;  ^^^^^  end of - OLD VERSIONS OF SCHEDULE DIALOGS AS SEPARATE TABBED DIALOGS  ^^^^^


 
 ;********************************************************************
 ;********************************************************************
 ;**
 ;**		Utility Rate Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************
MODTABDLG, 3070, 3071, 1, 100, 100, 470, 710, 0, UTILITY-RATE, "Utility Rate Properties", NOTIMP, 0, NOTIMP, 0
 
   COMBO, 15167, 0, 0, 1, UTILITY-RATE, 0, NAME,  0, STD, 190,  15, 400, 250, 19, 3, "Currently Active Utility Rate:",  LEFT, -175, 5, 0, LEFT, 4, 5, "List of all utility rates defined in project; also allows library retrieval and creation"
   STATIC, 1, UTILITY-RATE, 0, TYPE, 0, 0, 0, 460, 20, 250, STD, LEFT, "Service Type: ",   "", 0, 3
    
    ;*****************************************
    ; General Tab
    ;*****************************************
  TABPAGE, 3071, 3071, 1, 3, NOTIMP, " General "

    EDIT, 12299, 12299, 0, 1, UTILITY-RATE,  0,          NAME,   0, STD, 135,  10,  23, 230, 32, 3,  "Utility Rate Name:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Name of utility rate; right mouse quick menu options allow deleting, copying, linking and saving to library"
   COMBO, 12300, 12300, 0, 1, UTILITY-RATE,  0,          TYPE,   0, STD, 135,  35, 300, 230, 19, 3,       "Service Type:", RIGHT,  -10, 5, 0, LEFT, 4, 5, "Determines which fuel or energy type is being valued"
    
   LABEL, "Monthly Inputs", STD, LEFT,   410,  25, 1, 0, 0, 680, 0, 3
   LABEL, "Last Day in",    STD, CENTER, 537,  42, 1, 0, 0,   0, 15168, 3
   LABEL, "Billing Cycle",  STD, CENTER, 537,  58, 1, 0, 0,   0, 15168, 3
    EDIT, 15168, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   0, STD, 505,  75,  23,  65,  0, 3, "January:",    LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15169, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   1, STD, 505, 100,  23,  65,  0, 3, "February:",   LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15170, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   2, STD, 505, 125,  23,  65,  0, 3, "March:",      LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15171, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   3, STD, 505, 150,  23,  65,  0, 3, "April:",      LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15172, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   4, STD, 505, 175,  23,  65,  0, 3, "May:",        LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15173, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   5, STD, 505, 200,  23,  65,  0, 3, "June:",       LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15174, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   6, STD, 505, 225,  23,  65,  0, 3, "July:",       LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15175, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   7, STD, 505, 250,  23,  65,  0, 3, "August:",     LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15176, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   8, STD, 505, 275,  23,  65,  0, 3, "September:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15177, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,   9, STD, 505, 300,  23,  65,  0, 3, "October:",    LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15178, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,  10, STD, 505, 325,  23,  65,  0, 3, "November:",   LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"
    EDIT, 15179, 63103, 0, 1, UTILITY-RATE,  0,  BILLING-DAYS,  11, STD, 505, 350,  23,  65,  0, 3, "December:",   LEFT,  -75, 5, 1, LEFT, 4, 5, "Last day of the utility billing period (for each of the twelve months of the year)"

   LABEL, "Monthly",  STD, CENTER, 613,  42, 1, 0, 0,   0, 15180, 3
   LABEL, "Charges",  STD, CENTER, 613,  58, 1, 0, 0,   0, 15180, 3
    EDIT, 15180, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     0, STD, 580,  75,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15181, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     1, STD, 580, 100,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15182, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     2, STD, 580, 125,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15183, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     3, STD, 580, 150,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15184, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     4, STD, 580, 175,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15185, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     5, STD, 580, 200,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15186, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     6, STD, 580, 225,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15187, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     7, STD, 580, 250,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15188, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     8, STD, 580, 275,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15189, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,     9, STD, 580, 300,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15190, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,    10, STD, 580, 325,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"
    EDIT, 15191, 11546, 0, 1, UTILITY-RATE,  0,  MONTH-CHGS,    11, STD, 580, 350,  23,  65,  2, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "A fixed monthly charge added to each billing cycle (for each month)"

    ; STEAM Meters
    CASE,  UTILITY-RATE,  0, TYPE,  -1,  =, 1, 1
      LABEL, "Steam Meters Served", STD, LEFT, 20, 105, 1, 0, 0, 365, 0, 3
      COMBO, 15192, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   0, STD,  50, 125, 250,  75, 19, 3,   "1:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15193, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   1, STD,  50, 150, 250,  75, 19, 3,   "2:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15194, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   2, STD,  50, 175, 250,  75, 19, 3,   "3:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15195, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   3, STD,  50, 200, 250,  75, 19, 3,   "4:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15196, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   4, STD,  50, 225, 250,  75, 19, 3,   "5:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15197, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   5, STD,  50, 250, 250,  75, 19, 3,   "6:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15198, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   6, STD,  50, 275, 250,  75, 19, 3,   "7:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15199, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   7, STD,  50, 300, 250,  75, 19, 3,   "8:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15200, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   8, STD,  50, 325, 250,  75, 19, 3,   "9:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15201, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,   9, STD,  50, 350, 250,  75, 19, 3,  "10:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"

      COMBO, 15202, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  10, STD, 170, 125, 250,  75, 19, 3,  "11:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15203, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  11, STD, 170, 150, 250,  75, 19, 3,  "12:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15204, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  12, STD, 170, 175, 250,  75, 19, 3,  "13:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15205, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  13, STD, 170, 200, 250,  75, 19, 3,  "14:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15206, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  14, STD, 170, 225, 250,  75, 19, 3,  "15:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15207, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  15, STD, 170, 250, 250,  75, 19, 3,  "16:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15208, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  16, STD, 170, 275, 250,  75, 19, 3,  "17:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15209, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  17, STD, 170, 300, 250,  75, 19, 3,  "18:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15210, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  18, STD, 170, 325, 250,  75, 19, 3,  "19:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15211, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  19, STD, 170, 350, 250,  75, 19, 3,  "20:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"

      COMBO, 15212, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  20, STD, 290, 125, 250,  75, 19, 3,  "21:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15213, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  21, STD, 290, 150, 250,  75, 19, 3,  "22:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15214, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  22, STD, 290, 175, 250,  75, 19, 3,  "23:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15215, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  23, STD, 290, 200, 250,  75, 19, 3,  "24:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
      COMBO, 15216, 63097, 0, 1, UTILITY-RATE,  0, STEAM-METERS,  24, STD, 290, 225, 250,  75, 19, 3,  "25:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Steam meters assigned to this utility rate"
    ENDCASE

    ; CHW Meters
    CASE,  UTILITY-RATE,  0, TYPE,  -1,  =, 1, 2
      LABEL, "CHW Meters Served", STD, LEFT, 20, 105, 1, 0, 0, 365, 0, 3
      COMBO, 15192, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     0, STD,  50, 125, 250,  75, 19, 3,   "1:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15193, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     1, STD,  50, 150, 250,  75, 19, 3,   "2:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15194, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     2, STD,  50, 175, 250,  75, 19, 3,   "3:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15195, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     3, STD,  50, 200, 250,  75, 19, 3,   "4:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15196, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     4, STD,  50, 225, 250,  75, 19, 3,   "5:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15197, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     5, STD,  50, 250, 250,  75, 19, 3,   "6:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15198, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     6, STD,  50, 275, 250,  75, 19, 3,   "7:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15199, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     7, STD,  50, 300, 250,  75, 19, 3,   "8:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15200, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     8, STD,  50, 325, 250,  75, 19, 3,   "9:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15201, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,     9, STD,  50, 350, 250,  75, 19, 3,  "10:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"

      COMBO, 15202, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    10, STD, 170, 125, 250,  75, 19, 3,  "11:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15203, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    11, STD, 170, 150, 250,  75, 19, 3,  "12:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15204, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    12, STD, 170, 175, 250,  75, 19, 3,  "13:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15205, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    13, STD, 170, 200, 250,  75, 19, 3,  "14:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15206, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    14, STD, 170, 225, 250,  75, 19, 3,  "15:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15207, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    15, STD, 170, 250, 250,  75, 19, 3,  "16:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15208, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    16, STD, 170, 275, 250,  75, 19, 3,  "17:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15209, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    17, STD, 170, 300, 250,  75, 19, 3,  "18:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15210, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    18, STD, 170, 325, 250,  75, 19, 3,  "19:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15211, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    19, STD, 170, 350, 250,  75, 19, 3,  "20:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"

      COMBO, 15212, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    20, STD, 290, 125, 250,  75, 19, 3,  "21:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15213, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    21, STD, 290, 150, 250,  75, 19, 3,  "22:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15214, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    22, STD, 290, 175, 250,  75, 19, 3,  "23:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15215, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    23, STD, 290, 200, 250,  75, 19, 3,  "24:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
      COMBO, 15216, 63097, 0, 1, UTILITY-RATE,  0, CHW-METERS,    24, STD, 290, 225, 250,  75, 19, 3,  "25:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Chilled water meters assigned to this utility rate"
    ENDCASE

    ; Electric Meters
    CASE,  UTILITY-RATE,  0, TYPE,  -1,  =, 3, 3, 13, 14
      LABEL, "Electric Meters Served", STD, LEFT, 20, 105, 1, 0, 0, 365, 0, 3
      COMBO, 15192, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    0, STD,  50, 125, 250,  75, 19, 3,   "1:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15193, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    1, STD,  50, 150, 250,  75, 19, 3,   "2:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15194, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    2, STD,  50, 175, 250,  75, 19, 3,   "3:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15195, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    3, STD,  50, 200, 250,  75, 19, 3,   "4:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15196, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    4, STD,  50, 225, 250,  75, 19, 3,   "5:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15197, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    5, STD,  50, 250, 250,  75, 19, 3,   "6:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15198, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    6, STD,  50, 275, 250,  75, 19, 3,   "7:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15199, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    7, STD,  50, 300, 250,  75, 19, 3,   "8:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15200, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    8, STD,  50, 325, 250,  75, 19, 3,   "9:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15201, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,    9, STD,  50, 350, 250,  75, 19, 3,  "10:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"

      COMBO, 15202, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   10, STD, 170, 125, 250,  75, 19, 3,  "11:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15203, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   11, STD, 170, 150, 250,  75, 19, 3,  "12:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15204, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   12, STD, 170, 175, 250,  75, 19, 3,  "13:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15205, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   13, STD, 170, 200, 250,  75, 19, 3,  "14:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15206, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   14, STD, 170, 225, 250,  75, 19, 3,  "15:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15207, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   15, STD, 170, 250, 250,  75, 19, 3,  "16:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15208, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   16, STD, 170, 275, 250,  75, 19, 3,  "17:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15209, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   17, STD, 170, 300, 250,  75, 19, 3,  "18:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15210, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   18, STD, 170, 325, 250,  75, 19, 3,  "19:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15211, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   19, STD, 170, 350, 250,  75, 19, 3,  "20:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"

      COMBO, 15212, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   20, STD, 290, 125, 250,  75, 19, 3,  "21:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15213, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   21, STD, 290, 150, 250,  75, 19, 3,  "22:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15214, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   22, STD, 290, 175, 250,  75, 19, 3,  "23:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15215, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   23, STD, 290, 200, 250,  75, 19, 3,  "24:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
      COMBO, 15216, 63097, 0, 1, UTILITY-RATE,  0, ELEC-METERS,   24, STD, 290, 225, 250,  75, 19, 3,  "25:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Electric meters assigned to this utility rate"
    ENDCASE

    ; Fuel Meters
    CASE,  ELSE 
      LABEL, "Fuel Meters Served", STD, LEFT, 20, 105, 1, 0, 0, 365, 0, 3
      COMBO, 15192, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    0, STD,  50, 125, 250,  75, 19, 3,   "1:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15193, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    1, STD,  50, 150, 250,  75, 19, 3,   "2:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15194, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    2, STD,  50, 175, 250,  75, 19, 3,   "3:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15195, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    3, STD,  50, 200, 250,  75, 19, 3,   "4:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15196, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    4, STD,  50, 225, 250,  75, 19, 3,   "5:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15197, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    5, STD,  50, 250, 250,  75, 19, 3,   "6:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15198, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    6, STD,  50, 275, 250,  75, 19, 3,   "7:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15199, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    7, STD,  50, 300, 250,  75, 19, 3,   "8:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15200, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    8, STD,  50, 325, 250,  75, 19, 3,   "9:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15201, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,    9, STD,  50, 350, 250,  75, 19, 3,  "10:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"

      COMBO, 15202, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   10, STD, 170, 125, 250,  75, 19, 3,  "11:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15203, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   11, STD, 170, 150, 250,  75, 19, 3,  "12:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15204, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   12, STD, 170, 175, 250,  75, 19, 3,  "13:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15205, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   13, STD, 170, 200, 250,  75, 19, 3,  "14:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15206, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   14, STD, 170, 225, 250,  75, 19, 3,  "15:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15207, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   15, STD, 170, 250, 250,  75, 19, 3,  "16:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15208, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   16, STD, 170, 275, 250,  75, 19, 3,  "17:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15209, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   17, STD, 170, 300, 250,  75, 19, 3,  "18:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15210, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   18, STD, 170, 325, 250,  75, 19, 3,  "19:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15211, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   19, STD, 170, 350, 250,  75, 19, 3,  "20:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"

      COMBO, 15212, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   20, STD, 290, 125, 250,  75, 19, 3,  "21:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15213, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   21, STD, 290, 150, 250,  75, 19, 3,  "22:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15214, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   22, STD, 290, 175, 250,  75, 19, 3,  "23:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15215, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   23, STD, 290, 200, 250,  75, 19, 3,  "24:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
      COMBO, 15216, 63097, 0, 1, UTILITY-RATE,  0, FUEL-METERS,   24, STD, 290, 225, 250,  75, 19, 3,  "25:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Fuel meters assigned to this utility rate"
    ENDCASE  

    ;*****************************************
    ; Energy/Demand Tab
    ;*****************************************
  TABPAGE, 3072, 3072, 1, 3, NOTIMP, " Energy/Demand "
    
   LABEL, "Energy", STD, LEFT,  20, 30, 1, 0, 0, 345, 12319, 3
    EDIT, 12319, 12319,    0, 1, UTILITY-RATE, 0,      ENERGY-CHG,   0, STD, 185,  50,  23, 110,  6, 3, "Uniform Energy Charge:*",  LEFT, -155, 5, 1, LEFT, 4, 5, "An energy charge that is constant with time of use and fuel Type"
   COMBO, 12320, 12320,    0, 1, UTILITY-RATE, 0,  ENERGY-CHG-SCH,   0, STD, 185,  75, 200, 160, 19, 3, "Energy Charge Schedule:",  LEFT, -155, 5, 0, LEFT, 4, 5, "A schedule that defines Energy Cost Adjustment charges (on an hourly basis)"
   
   LABEL, "* For energy charges defined by usage blocks select the", ITALIC, LEFT,  30, 106, 1, 0, 0, 0, 0, 3
   LABEL, "'Examine Block Charges' button on the 'Blocks' tab.",     ITALIC, LEFT,  40, 122, 1, 0, 0, 0, 0, 3
   
   LABEL, "Metered Demand Time Interval", STD, LEFT,  20, 180, 1, 0, 0, 285, 12346, 3
   COMBO, 12346, 12346, 3073, 1, UTILITY-RATE, 0,   DEMAND-WINDOW,   0, STD, 185, 200, 200, 100, 19, 3,          "Demand Window:",  LEFT, -145, 5, 0, LEFT, 4, 5, ""
    EDIT, 14416, 14416, 3073, 1, UTILITY-RATE, 0, DEMAND-INTERVAL,   0, STD, 185, 225,  23,  80,  0, 3,        "Demand Interval:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Length of the time window in which peak demand is calculated"
   
   LABEL, "Monthly Demand Charges", STD, LEFT,  440, 30, 1, 0, 0, 680, 0, 3
    EDIT, 15216, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   0, STD, 545,  50,  23,  70,  3, 3, "January:",    LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15217, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   1, STD, 545,  75,  23,  70,  3, 3, "February:",   LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15218, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   2, STD, 545, 100,  23,  70,  3, 3, "March:",      LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15219, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   3, STD, 545, 125,  23,  70,  3, 3, "April:",      LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15220, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   4, STD, 545, 150,  23,  70,  3, 3, "May:",        LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15221, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   5, STD, 545, 175,  23,  70,  3, 3, "June:",       LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15222, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   6, STD, 545, 200,  23,  70,  3, 3, "July:",       LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15223, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   7, STD, 545, 225,  23,  70,  3, 3, "August:",     LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15224, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   8, STD, 545, 250,  23,  70,  3, 3, "September:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15225, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,   9, STD, 545, 275,  23,  70,  3, 3, "October:",    LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15226, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,  10, STD, 545, 300,  23,  70,  3, 3, "November:",   LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    EDIT, 15227, 11528, 3073, 1, UTILITY-RATE,  0,    DEMAND-CHGS,  11, STD, 545, 325,  23,  70,  3, 3, "December:",   LEFT,  -75, 5, 1, LEFT, 4, 5, "Dollars per peak unit:if less than 12 entries, the last one applies to all remaining billing periods"
    
    ;*****************************************
    ; Blocks Tab
    ;*****************************************
  TABPAGE, 3074, 3074, 1, 3, NOTIMP, " Blocks "
    
   LABEL, "Block Charges Assigned To This Rate", STD, LEFT, 20, 30, 1, 0, 0, 520, 0, 3

   COMBO, 15228, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   0, STD,  60,  50, 250, 200, 19, 3,   "1:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15229, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   1, STD,  60,  75, 250, 200, 19, 3,   "2:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15230, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   2, STD,  60, 100, 250, 200, 19, 3,   "3:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15231, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   3, STD,  60, 125, 250, 200, 19, 3,   "4:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15232, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   4, STD,  60, 150, 250, 200, 19, 3,   "5:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15233, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   5, STD,  60, 175, 250, 200, 19, 3,   "6:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15234, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   6, STD,  60, 200, 250, 200, 19, 3,   "7:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15235, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   7, STD,  60, 225, 250, 200, 19, 3,   "8:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15236, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   8, STD,  60, 250, 250, 200, 19, 3,   "9:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15237, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,   9, STD,  60, 275, 250, 200, 19, 3,  "10:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"

   COMBO, 15238, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  10, STD, 320,  50, 250, 200, 19, 3,  "11:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15239, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  11, STD, 320,  75, 250, 200, 19, 3,  "12:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15240, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  12, STD, 320, 100, 250, 200, 19, 3,  "13:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15241, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  13, STD, 320, 125, 250, 200, 19, 3,  "14:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15242, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  14, STD, 320, 150, 250, 200, 19, 3,  "15:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15243, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  15, STD, 320, 175, 250, 200, 19, 3,  "16:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15244, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  16, STD, 320, 200, 250, 200, 19, 3,  "17:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15245, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  17, STD, 320, 225, 250, 200, 19, 3,  "18:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15246, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  18, STD, 320, 250, 250, 200, 19, 3,  "19:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"
   COMBO, 15247, 12450, 0, 1, UTILITY-RATE,  0, BLOCK-CHARGES,  19, STD, 320, 275, 250, 200, 19, 3,  "20:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Block charges assigned to this rate (up to 20 block charges per utility rate)"

  BUTTON, 10271, 3080, 0, 1, 92, 3081, STD, 510, 355, 23, 180, 3, "Examine Block Charges...", "" 	

    ;*****************************************
    ; Ratchets Tab
    ;*****************************************
  TABPAGE, 3075, 3075, 1, 3, NOTIMP, " Ratchets "
    
   LABEL, "General Ratchets Assigned To This Rate", STD, LEFT, 20, 20, 1, 0, 0, 680, 15248, 3

   COMBO, 15248, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   0, STD,  60,  40, 250, 170, 19, 3,   "1:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15249, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   1, STD,  60,  65, 250, 170, 19, 3,   "2:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15250, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   2, STD,  60,  90, 250, 170, 19, 3,   "3:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15251, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   3, STD,  60, 115, 250, 170, 19, 3,   "4:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15252, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   4, STD,  60, 140, 250, 170, 19, 3,   "5:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"

   COMBO, 15253, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   5, STD, 285,  40, 250, 170, 19, 3,   "6:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15254, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   6, STD, 285,  65, 250, 170, 19, 3,   "7:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15255, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   7, STD, 285,  90, 250, 170, 19, 3,   "8:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15256, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   8, STD, 285, 115, 250, 170, 19, 3,   "9:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15257, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,   9, STD, 285, 140, 250, 170, 19, 3,  "10:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"

   COMBO, 15258, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,  10, STD, 510,  40, 250, 170, 19, 3,  "11:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15259, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,  11, STD, 510,  65, 250, 170, 19, 3,  "12:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15260, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,  12, STD, 510,  90, 250, 170, 19, 3,  "13:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15261, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,  13, STD, 510, 115, 250, 170, 19, 3,  "14:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"
   COMBO, 15262, 11530, 0, 1, UTILITY-RATE,  0, DEMAND-RATCHETS,  14, STD, 510, 140, 250, 170, 19, 3,  "15:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify billing demands (up to 15 ratchets per utility rate)"

   LABEL, "Minimum Ratchets Assigned To This Rate*", STD, LEFT, 20, 185, 1, 0, 0, 680, 15263, 3

   COMBO, 15263, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  0, STD,  60, 205, 250, 170, 19, 3,   "1:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15264, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  1, STD,  60, 230, 250, 170, 19, 3,   "2:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15265, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  2, STD,  60, 255, 250, 170, 19, 3,   "3:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15266, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  3, STD,  60, 280, 250, 170, 19, 3,   "4:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15267, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  4, STD,  60, 305, 250, 170, 19, 3,   "5:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"

   COMBO, 15268, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  5, STD, 285, 205, 250, 170, 19, 3,   "6:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15269, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  6, STD, 285, 230, 250, 170, 19, 3,   "7:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15270, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  7, STD, 285, 255, 250, 170, 19, 3,   "8:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15271, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  8, STD, 285, 280, 250, 170, 19, 3,   "9:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15272, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS,  9, STD, 285, 305, 250, 170, 19, 3,  "10:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"

   COMBO, 15273, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS, 10, STD, 510, 205, 250, 170, 19, 3,  "11:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15274, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS, 11, STD, 510, 230, 250, 170, 19, 3,  "12:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15275, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS, 12, STD, 510, 255, 250, 170, 19, 3,  "13:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15276, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS, 13, STD, 510, 280, 250, 170, 19, 3,  "14:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"
   COMBO, 15277, 63098, 0, 1, UTILITY-RATE,  0, MIN-MON-RATCHETS, 14, STD, 510, 305, 250, 170, 19, 3,  "15:",  LEFT,  -25, 5, 0, LEFT, 4, 5, "Ratchets that modify demand for minimum monthly demand charges"

   LABEL, "* Minimum ratchets are only used with minimum monthly charge calculations", ITALIC, LEFT, 35, 333, 1, 0, 0, 0, 15263, 3

  BUTTON, 10272, 2515, 0, 1, 92, 3200, STD, 510, 355, 23, 180, 3, "Examine Ratchets...", "" 	
    
    ;*****************************************
    ; Min/Max Chgs Tab
    ;*****************************************
  TABPAGE, 3076, 3076, 1, 3, NOTIMP, " Min/Max Charges "
    
   LABEL, "Minimum Monthly Charges Based On*", STD, LEFT,  20,   5, 1, 0, 0, 330, 0, 3
   LABEL, "Fixed",         STD, CENTER, 157,  22, 1, 0, 0,   0, 15278, 3
   LABEL, "Chrgs ($/mon)", STD, CENTER, 157,  38, 1, 0, 0,   0, 15278, 3
    EDIT, 15278, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  0, STD, 115,  55,  23,  85,  3, 3, "January:",    LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15279, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  1, STD, 115,  80,  23,  85,  3, 3, "February:",   LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15280, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  2, STD, 115, 105,  23,  85,  3, 3, "March:",      LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15281, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  3, STD, 115, 130,  23,  85,  3, 3, "April:",      LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15282, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  4, STD, 115, 155,  23,  85,  3, 3, "May:",        LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15283, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  5, STD, 115, 180,  23,  85,  3, 3, "June:",       LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15284, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  6, STD, 115, 205,  23,  85,  3, 3, "July:",       LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15285, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  7, STD, 115, 230,  23,  85,  3, 3, "August:",     LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15286, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  8, STD, 115, 255,  23,  85,  3, 3, "September:",  LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15287, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS,  9, STD, 115, 280,  23,  85,  3, 3, "October:",    LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15288, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS, 10, STD, 115, 305,  23,  85,  3, 3, "November:",   LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"
    EDIT, 15289, 11531, 0, 1, UTILITY-RATE,  0,     MIN-MON-CHGS, 11, STD, 115, 330,  23,  85,  3, 3, "December:",   LEFT,  -75, 5, 0, LEFT, 4, 5, "Minimum fixed charge for a billing period (for each month)"

   LABEL, "Min Peak",     STD, CENTER, 253,  22, 1, 0, 0,   0, 15290, 3
   LABEL, "Demand Chrgs", STD, CENTER, 253,  38, 1, 0, 0,   0, 15290, 3
    EDIT, 15290, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  0, STD, 210,  55,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15291, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  1, STD, 210,  80,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15292, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  2, STD, 210, 105,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15293, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  3, STD, 210, 130,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15294, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  4, STD, 210, 155,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15295, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  5, STD, 210, 180,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15296, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  6, STD, 210, 205,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15297, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  7, STD, 210, 230,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15298, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  8, STD, 210, 255,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15299, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS,  9, STD, 210, 280,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15300, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS, 10, STD, 210, 305,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"
    EDIT, 15301, 63104, 0, 1, UTILITY-RATE,  0, MIN-MON-DEM-CHGS, 11, STD, 210, 330,  23,  85,  3, 3, "",            LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum charge, based on peak demand, for a billing period (for each month)"

   LABEL, "* Total minimum monthly charges will be the sum of these two columns.  This total", ITALIC, LEFT, 40, 358, 1, 0, 0, 0, 0, 3
   LABEL, "excludes any customer charges, taxes, surcharges, or energy cost adjustments.",     ITALIC, LEFT, 50, 374, 1, 0, 0, 0, 0, 3

   LABEL, "Rate Limitation", STD, LEFT, 380,  35, 1, 0, 0, 675, 12413, 3
    EDIT, 12413, 12413,    0, 1, UTILITY-RATE,  0,  RATE-LIMITATION,  0, STD, 560,  55,  23,  85,  2, 3,   "Maximum Effective Rate:",  LEFT, -165, 5, 1, LEFT, 4, 5, "Maximum effective charge ($ per unit) assessed on a utility or fuel for any month"

   LABEL, "Minimum Energy & Demand", STD, LEFT, 380, 110, 1, 0, 0, 675, 12412, 3
   COMBO, 12412, 12412, 3079, 1, UTILITY-RATE,  0,    USE-MIN-QUALS,  0, STD, 560, 130,  85,  85, 19, 3,  "Use Min Rate Qualifiers:",  LEFT, -165, 5, 0, LEFT, 4, 5, "Whether there is a minimum charge calculation for either energy or demand"

    CASE,  UTILITY-RATE,  0, USE-MIN-QUALS,  -1,  =, 1, 1
       EDIT, 12304, 12304, 3079, 1, UTILITY-RATE,  0,  ENERGY-QUALS,  0, STD, 560, 155,  23,  85,  2, 3, "Minimum Billing Energy**:",  LEFT, -165, 5, 1, LEFT, 4, 5, "Minimum monthly energy usage that determines if this rate applies"
       EDIT, 12305, 12305, 3079, 1, UTILITY-RATE,  0,  DEMAND-QUALS,  0, STD, 560, 180,  23,  85,  2, 3, "Minimum Billing Demand**:",  LEFT, -165, 5, 1, LEFT, 4, 5, "Minimum demand that will be billed (used only if Use Minimum Rate Qualifiers = Yes)"
      LABEL, "** These fields also used for Minimum Monthly",  ITALIC, LEFT, 395, 208, 1, 0, 0, 0, 0, 3
      LABEL,   "Energy Usage and Minimum Monthly Peak",        ITALIC, LEFT, 410, 224, 1, 0, 0, 0, 0, 3
      LABEL,   "Demand.  See 'Qualifiers' tab.",               ITALIC, LEFT, 410, 240, 1, 0, 0, 0, 0, 3
    ENDCASE    
   
    ;*****************************************
    ; Adjustments Tab
    ;*****************************************
  TABPAGE, 3077, 3077, 1, 3, NOTIMP, " Adjust/Escalation "
    
   LABEL, "Monthly Energy Cost Adjustments", STD, LEFT,  20, 30, 1, 0, 0, 245, 0, 3
    EDIT, 15302, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   0, STD, 125,  50,  23,  90,  6, 3, "January:",    LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15303, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   1, STD, 125,  75,  23,  90,  6, 3, "February:",   LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15304, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   2, STD, 125, 100,  23,  90,  6, 3, "March:",      LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15305, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   3, STD, 125, 125,  23,  90,  6, 3, "April:",      LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15306, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   4, STD, 125, 150,  23,  90,  6, 3, "May:",        LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15307, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   5, STD, 125, 175,  23,  90,  6, 3, "June:",       LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15308, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   6, STD, 125, 200,  23,  90,  6, 3, "July:",       LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15309, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   7, STD, 125, 225,  23,  90,  6, 3, "August:",     LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15310, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   8, STD, 125, 250,  23,  90,  6, 3, "September:",  LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15311, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,   9, STD, 125, 275,  23,  90,  6, 3, "October:",    LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15312, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,  10, STD, 125, 300,  23,  90,  6, 3, "November:",   LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"
    EDIT, 15313, 11532, 0, 1, UTILITY-RATE,  0,  ENERGY-COST-ADJS,  11, STD, 125, 325,  23,  90,  6, 3, "December:",   LEFT,  -75, 5, 1, LEFT, 4, 5, "Energy cost adjustment factor for each billing period: multiplied by total monthly energy use"

   LABEL, "Energy Cost Adjustments", STD, LEFT,  325, 30, 1, 0, 0, 665, 12438, 3
   COMBO, 12438, 12438, 0, 1, UTILITY-RATE, 0,    ENERGY-ADJ-SCH,    0, STD, 485,  50, 200, 180, 19, 3,   "Adjustment Schedule:",  LEFT, -140, 5, 0, LEFT, 4, 5, "A schedule that defines Energy Cost Adjustment charges (on an hourly basis)"
    
   LABEL, "Annual Utility Price Escalation Rate", STD, LEFT,  325, 105, 1, 0, 0, 585, 14331, 3
    EDIT, 14331, 12318, 0, 1, UTILITY-RATE, 0,    ESCALATION,        0, STD, 485, 125,  23,  70,  3, 3,            "Escalation:",  LEFT, -140, 5, 1, LEFT, 4, 5, ""
   
   LABEL, "Power Factor Adjustments", STD, LEFT,  325, 180, 1, 0, 0, 585, 12439, 3
    EDIT, 12439, 12439, 0, 1, UTILITY-RATE, 0,    POWER-FACTOR,      0, STD, 485, 200,  23,  70,  3, 3,          "Power Factor:",  LEFT, -140, 5, 1, LEFT, 4, 5, "Fraction of peak kVA due to real power"
    EDIT, 12440, 12440, 0, 1, UTILITY-RATE, 0,    EXCESS-KVAR-FRAC,  0, STD, 485, 225,  23,  70,  3, 3,  "Excess kVAR Fraction:",  LEFT, -140, 5, 1, LEFT, 4, 5, "Fraction of real kW above which a charge is levied (I.e., Excess kVAR Charge applies)"
    EDIT, 12441, 12441, 0, 1, UTILITY-RATE, 0,    EXCESS-KVAR-CHG,   0, STD, 485, 250,  23,  70,  3, 3,    "Excess kVAR Charge:",  LEFT, -140, 5, 1, LEFT, 4, 5, "Charge for excess reactive demand ($/kVAR)"
    
    ;*****************************************
    ; Taxes Tab
    ;*****************************************
  TABPAGE, 3078, 3078, 1, 3, NOTIMP, " Taxes "
    
   LABEL, "Surcharges Apply To", STD, LEFT,  40,  5, 1, 0, 0, 310, 12729, 3
   COMBO, 12729, 12729, 0, 1, UTILITY-RATE, 0, PCT-SRCHGS-APPLY,  0, STD, 120,  25, 200, 190, 19, 3,           "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "The categories of charges upon which surcharges are levied"
   COMBO, 12730, 12729, 0, 1, UTILITY-RATE, 0, PCT-SRCHGS-APPLY,  1, STD, 120,  50, 200, 190, 19, 3,           "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "The categories of charges upon which surcharges are levied"
   COMBO, 12731, 12729, 0, 1, UTILITY-RATE, 0, PCT-SRCHGS-APPLY,  2, STD, 120,  75, 200, 190, 19, 3,           "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "The categories of charges upon which surcharges are levied"
    
   LABEL, "Percent Surcharge Data", STD, LEFT,  40, 121, 1, 0, 0, 310, 15314, 3
   LABEL, "Block Size ($)",  STD, CENTER,  165, 138, 1, 0, 0, 0, 0, 3
   LABEL, "Surcharge (%)",  STD, CENTER,  265, 138, 1, 0, 0, 0, 0, 3
    EDIT, 15314, 11533, 0, 1, UTILITY-RATE, 0, PCT-SRCHG-BLOCKS,  0, STD, 120, 155,  23,  90,  3, 3,   "Block 1:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of the block of money upon which a surcharge will be levied (on a % basis)"
    EDIT, 15315, 63099, 0, 1, UTILITY-RATE, 0,       PCT-SRCHGS,  0, STD, 220, 155,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Surcharge in % (up to 3 - corresponding to blocks in Percent Surcharge Data Block Size)"
    EDIT, 15316, 11533, 0, 1, UTILITY-RATE, 0, PCT-SRCHG-BLOCKS,  1, STD, 120, 180,  23,  90,  3, 3,   "Block 2:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of the block of money upon which a surcharge will be levied (on a % basis)"
    EDIT, 15317, 63099, 0, 1, UTILITY-RATE, 0,       PCT-SRCHGS,  1, STD, 220, 180,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Surcharge in % (up to 3 - corresponding to blocks in Percent Surcharge Data Block Size)"
    EDIT, 15318, 11533, 0, 1, UTILITY-RATE, 0, PCT-SRCHG-BLOCKS,  2, STD, 120, 205,  23,  90,  3, 3,   "Block 3:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of the block of money upon which a surcharge will be levied (on a % basis)"
    EDIT, 15319, 63099, 0, 1, UTILITY-RATE, 0,       PCT-SRCHGS,  2, STD, 220, 205,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Surcharge in % (up to 3 - corresponding to blocks in Percent Surcharge Data Block Size)"
    
   LABEL, "Unit Surcharge Data", STD, LEFT,  40, 250, 1, 0, 0, 310, 15320, 3
   LABEL, "Block Size",      STD, CENTER,  165, 267, 1, 0, 0, 0, 0, 3
   LABEL, "(energy units)",  STD, CENTER,  165, 283, 1, 0, 0, 0, 0, 3
   LABEL, "Charge",           STD, CENTER,  265, 268, 1, 0, 0, 0, 0, 3
   LABEL, "($/energy unit)",  STD, CENTER,  265, 284, 1, 0, 0, 0, 0, 3
    EDIT, 15320, 11534, 0, 1, UTILITY-RATE, 0, UNIT-SRCHG-BLOCK,  0, STD, 120, 300,  23,  90,  3, 3,   "Block 1:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of block of energy on which a surcharge is levied (per energy unit basis)"
    EDIT, 15321, 63100, 0, 1, UTILITY-RATE, 0,      UNIT-SRCHGS,  0, STD, 220, 300,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Surcharge in $/energy unit  (up to 3 - corresponding to Unit Surcharge Data Block Size)"
    EDIT, 15322, 11534, 0, 1, UTILITY-RATE, 0, UNIT-SRCHG-BLOCK,  1, STD, 120, 325,  23,  90,  3, 3,   "Block 2:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of block of energy on which a surcharge is levied (per energy unit basis)"
    EDIT, 15323, 63100, 0, 1, UTILITY-RATE, 0,      UNIT-SRCHGS,  1, STD, 220, 325,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Surcharge in $/energy unit  (up to 3 - corresponding to Unit Surcharge Data Block Size)"
    EDIT, 15324, 11534, 0, 1, UTILITY-RATE, 0, UNIT-SRCHG-BLOCK,  2, STD, 120, 350,  23,  90,  3, 3,   "Block 3:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of block of energy on which a surcharge is levied (per energy unit basis)"
    EDIT, 15325, 63100, 0, 1, UTILITY-RATE, 0,      UNIT-SRCHGS,  2, STD, 220, 350,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Surcharge in $/energy unit  (up to 3 - corresponding to Unit Surcharge Data Block Size)"

   LABEL, "Taxes Apply To", STD, LEFT, 380,  5, 1, 0, 0, 650, 12744, 3
   COMBO, 12744, 63105, 0, 1, UTILITY-RATE, 0,  PCT-TAXES-APPLY,  0, STD, 460,  25, 200, 190, 19, 3,           "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "The categories of charges upon which taxes are levied"
   COMBO, 12745, 63105, 0, 1, UTILITY-RATE, 0,  PCT-TAXES-APPLY,  1, STD, 460,  50, 200, 190, 19, 3,           "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "The categories of charges upon which taxes are levied"
   COMBO, 12746, 63105, 0, 1, UTILITY-RATE, 0,  PCT-TAXES-APPLY,  2, STD, 460,  75, 200, 190, 19, 3,           "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "The categories of charges upon which taxes are levied"
    
   LABEL, "Percent Tax Data", STD, LEFT, 380, 121, 1, 0, 0, 650, 15326, 3
   LABEL, "Block Size ($)",  STD, CENTER,  505, 138, 1, 0, 0, 0, 0, 3
   LABEL, "Tax Rate (%)",  STD, CENTER,  605, 138, 1, 0, 0, 0, 0, 3
    EDIT, 15326, 11535, 0, 1, UTILITY-RATE, 0,   PCT-TAX-BLOCKS,  0, STD, 460, 155,  23,  90,  3, 3,   "Block 1:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of the block of money upon which a tax will be levied (on a % basis)"
    EDIT, 15327, 63101, 0, 1, UTILITY-RATE, 0,        PCT-TAXES,  0, STD, 560, 155,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "The tax in % (up to 3 - corresponding to blocks in Percent Tax Data Block Size)"
    EDIT, 15328, 11535, 0, 1, UTILITY-RATE, 0,   PCT-TAX-BLOCKS,  1, STD, 460, 180,  23,  90,  3, 3,   "Block 2:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of the block of money upon which a tax will be levied (on a % basis)"
    EDIT, 15329, 63101, 0, 1, UTILITY-RATE, 0,        PCT-TAXES,  1, STD, 560, 180,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "The tax in % (up to 3 - corresponding to blocks in Percent Tax Data Block Size)"
    EDIT, 15330, 11535, 0, 1, UTILITY-RATE, 0,   PCT-TAX-BLOCKS,  2, STD, 460, 205,  23,  90,  3, 3,   "Block 3:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of the block of money upon which a tax will be levied (on a % basis)"
    EDIT, 15331, 63101, 0, 1, UTILITY-RATE, 0,        PCT-TAXES,  2, STD, 560, 205,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "The tax in % (up to 3 - corresponding to blocks in Percent Tax Data Block Size)"
    
   LABEL, "Unit Tax Data", STD, LEFT, 380, 250, 1, 0, 0, 650, 15320, 3
   LABEL, "Block Size",      STD, CENTER,  505, 267, 1, 0, 0, 0, 0, 3
   LABEL, "(energy units)",  STD, CENTER,  505, 283, 1, 0, 0, 0, 0, 3
   LABEL, "Charge",           STD, CENTER,  605, 268, 1, 0, 0, 0, 0, 3
   LABEL, "($/energy unit)",  STD, CENTER,  605, 284, 1, 0, 0, 0, 0, 3
    EDIT, 15332, 11536, 0, 1, UTILITY-RATE, 0,  UNIT-TAX-BLOCKS,  0, STD, 460, 300,  23,  90,  3, 3,   "Block 1:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of the block of energy upon which a tax is levied (per energy unit basis)"
    EDIT, 15333, 63102, 0, 1, UTILITY-RATE, 0,       UNIT-TAXES,  0, STD, 560, 300,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Tax in $/energy unit  (up to 3 - corresponding to Unit Tax Data Block Size)"
    EDIT, 15334, 11536, 0, 1, UTILITY-RATE, 0,  UNIT-TAX-BLOCKS,  1, STD, 460, 325,  23,  90,  3, 3,   "Block 2:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of the block of energy upon which a tax is levied (per energy unit basis)"
    EDIT, 15335, 63102, 0, 1, UTILITY-RATE, 0,       UNIT-TAXES,  1, STD, 560, 325,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Tax in $/energy unit  (up to 3 - corresponding to Unit Tax Data Block Size)"
    EDIT, 15336, 11536, 0, 1, UTILITY-RATE, 0,  UNIT-TAX-BLOCKS,  2, STD, 460, 350,  23,  90,  3, 3,   "Block 3:",  LEFT,  -60, 5, 1, LEFT, 4, 5, "Maximum size of the block of energy upon which a tax is levied (per energy unit basis)"
    EDIT, 15337, 63102, 0, 1, UTILITY-RATE, 0,       UNIT-TAXES,  2, STD, 560, 350,  23,  90,  4, 3,           "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Tax in $/energy unit  (up to 3 - corresponding to Unit Tax Data Block Size)"


    ;*****************************************
    ; Qualifiers Tab
    ;*****************************************
  TABPAGE, 3079, 3079, 1, 3, NOTIMP, " Qualifiers "
    
   LABEL, "Rate Qualifiers", STD, LEFT,  20,  16, 1, 0, 0, 350, 0, 3
   
   LABEL, "Minimum*", STD, CENTER,  222,  33, 1, 0, 0, 0, 0, 3
   LABEL, "Maximum",  STD, CENTER,  298,  33, 1, 0, 0, 0, 0, 3
    EDIT, 12442, 12442,    0, 1, UTILITY-RATE, 0, ENERGY-QUALS,  0, STD, 190,  50,  23,  65,  2, 3,   "Monthly Energy Usage:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Minimum monthly energy usage that determines if this rate applies"
    EDIT, 12443, 12443,    0, 1, UTILITY-RATE, 0, ENERGY-QUALS,  1, STD, 265,  50,  23,  65,  2, 3,                        "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum monthly energy usage that determines if this rate applies"

    EDIT, 12444, 12444, 3075, 1, UTILITY-RATE, 0, DEMAND-QUALS,  0, STD, 190,  75,  23,  65,  2, 3,    "Monthly Peak Demand:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Minimum demand that will be billed (used only if Use Minimum Rate Qualifiers = Yes)"
    EDIT, 12445, 12445, 3075, 1, UTILITY-RATE, 0, DEMAND-QUALS,  1, STD, 265,  75,  23,  65,  2, 3,                        "",  LEFT,   -2, 5, 1, LEFT, 4, 5, "Minimum demand that will be billed (used only if Use Minimum Rate Qualifiers = Yes)"
    
   COMBO, 12446, 12446,    0, 1, UTILITY-RATE, 0, QUALIFY-RATE,  0, STD, 190, 100, 200, 160, 19, 3,     "Rate Qualification:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Defines how energy & demand qualifiers are used to determine if this rate qualifies for use"
   COMBO, 12447, 12447,    0, 1, UTILITY-RATE, 0,     QUAL-SCH,  0, STD, 190, 125, 200, 160, 19, 3, "Qualification Schedule:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Name of schedule that defines the period(s) during which this utility rate may be used"
    
    EDIT, 12448, 12448,    0, 1, UTILITY-RATE, 0,     SCH-FLAG,  0, STD, 190, 150,  21,  40,  2, 3,    "Schedule Flag Value:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Flag value in the Qualification Schedule that activates this Utility Rate"
    
   LABEL, "* These fields can also be used for Minimum Billing Energy and Minimum Billing Demand.", ITALIC, LEFT,  40, 358, 1, 0, 0, 0, 0, 3
   LABEL, "See the Min/Max Charges tab.",                                                           ITALIC, LEFT,  50, 374, 1, 0, 0, 0, 0, 3

    

 ;********************************************************************
 ;********************************************************************
 ;**
 ;**		Block Charges Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************
MODTABDLG, 3080, 3074, 1, 100, 100, 470, 710, 0, BLOCK-CHARGE, "Block Charge Properties", NOTIMP, 0, NOTIMP, 0 
    
   COMBO, 12449, 12449, 0, 1, BLOCK-CHARGE, 0, NAME,  0, STD, 200,  15, 400, 250, 19, 3, "Currently Active Block Charge:",  LEFT, -185, 5, 0, LEFT, 4, 5, "List of all block charges defined in project; also allows library retrieval and creation"
    
    ;*****************************************
    ; Basic Specifications Tab
    ;*****************************************
  TABPAGE, 3081, 3074, 1, 3, NOTIMP, " Basic Specifications "
    
    EDIT, 12450,  1005, 0, 1, BLOCK-CHARGE, 0,             NAME,  0, STD, 160,  10,  23, 230, 32, 3,   "Block Charge Name:",  LEFT, -140, 5, 1, LEFT, 4, 5, "Name of block charge; right mouse quick menu options allow deleting, copying, linking and saving to library"

   COMBO, 12451, 12451, 0, 1, BLOCK-CHARGE, 0,       BLOCKS-ARE,  0, STD, 160,  75, 200, 160, 19, 3, "Energy Block Format:",  LEFT, -140, 5, 0, LEFT, 4, 5, "Whether energy blocks are defined as cumulative or incremental"
   COMBO, 12452, 12452, 0, 1, BLOCK-CHARGE, 0,        BLOCK-SCH,  0, STD, 160, 100, 200, 160, 19, 3,      "Block Schedule:",  LEFT, -140, 5, 0, LEFT, 4, 5, "Name of schedule that defines the period over which energy or demand is accumulated"
    EDIT, 12453, 12453, 0, 1, BLOCK-CHARGE, 0,         SCH-FLAG,  0, STD, 160, 125,  23,  60,  2, 3, "Schedule Flag Value:",  LEFT, -140, 5, 0, LEFT, 4, 5, "Flag value in the Block Schedule that indicates when this block charge is active"
   COMBO, 12454, 12454, 0, 1, BLOCK-CHARGE, 0, TOU-SEASON-LINKS,  0, STD, 160, 150, 200, 160, 19, 3,    "TOU Season Links:",  LEFT, -140, 5, 0, LEFT, 4, 5, "Name(s) of other block charge(s) that share the same billing period"
   COMBO, 12455, 12454, 0, 1, BLOCK-CHARGE, 0, TOU-SEASON-LINKS,  1, STD, 330, 150, 200, 160, 19, 3,                     "",  LEFT,   -2, 5, 0, LEFT, 4, 5, "Name(s) of other block charge(s) that share the same billing period"
    
   LABEL, "Ratchets Assigned To This Block", STD, LEFT,  20, 205, 1, 0, 0, 270, 15338, 3
   COMBO, 15338, 11537, 0, 1, BLOCK-CHARGE, 0,  DEMAND-RATCHETS,  0, STD,  70, 225, 250, 200, 19, 3,   "1:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Names of up to 5 ratchets that modify the billing demands for all demand charges"
   COMBO, 15339, 11537, 0, 1, BLOCK-CHARGE, 0,  DEMAND-RATCHETS,  1, STD,  70, 250, 250, 200, 19, 3,   "2:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Names of up to 5 ratchets that modify the billing demands for all demand charges"
   COMBO, 15340, 11537, 0, 1, BLOCK-CHARGE, 0,  DEMAND-RATCHETS,  2, STD,  70, 275, 250, 200, 19, 3,   "3:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Names of up to 5 ratchets that modify the billing demands for all demand charges"
   COMBO, 15341, 11537, 0, 1, BLOCK-CHARGE, 0,  DEMAND-RATCHETS,  3, STD,  70, 300, 250, 200, 19, 3,   "4:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Names of up to 5 ratchets that modify the billing demands for all demand charges"
   COMBO, 15342, 11537, 0, 1, BLOCK-CHARGE, 0,  DEMAND-RATCHETS,  4, STD,  70, 325, 250, 200, 19, 3,   "5:",  LEFT,  -20, 5, 0, LEFT, 4, 5, "Names of up to 5 ratchets that modify the billing demands for all demand charges"

  BUTTON, 10205, 2515, 0, 1, 92, 3200, STD, 510, 355, 23, 180, 3, "Examine Ratchets...", "" 	

    ;*****************************************
    ; Block 1 Tab
    ;*****************************************
  TABPAGE, 3082, 3074, 1, 3, NOTIMP, " Block 1 "

   STATIC, 1, BLOCK-CHARGE,  0, BLOCKS-ARE, 0, 0, 0, 30, 30, -1, STD, LEFT, "Energy Block Format:   ", "", 0, 3
   COMBO, 12499, 12499, 0, 1, BLOCK-CHARGE, 0, BLOCK1-TYPE,  0, STD, 110,  75, 200, 160, 19, 3,  "Block Type:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Type of block calculation; specifies the basis of block charges for this block"
    
    CASE,  BLOCK-CHARGE,  0, BLOCK1-TYPE,  -1,  =, 1, 1
       CASE,  BLOCK-CHARGE,  0, BLOCKS-ARE,  -1,  =, 1, 1
         LABEL, "Cumulative Limit",   STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "(block type unit)",  STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE     
       CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE
    ENDCASE    
    CASE, BLOCK-CHARGE, 0, BLOCK1-TYPE, -1, =, 2, 2, 3
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"

         LABEL, "Limit (block",  STD, CENTER, 623,  42, 1, 0, 0,   0, 15362, 3
         LABEL, "type unit)",    STD, CENTER, 623,  58, 1, 0, 0,   0, 15362, 3
          EDIT, 15362, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   0, STD, 580,  75,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15363, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   1, STD, 580, 100,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15364, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   2, STD, 580, 125,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15365, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   3, STD, 580, 150,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15366, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   4, STD, 580, 175,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15367, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   5, STD, 580, 200,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15368, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   6, STD, 580, 225,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15369, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   7, STD, 580, 250,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15370, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   8, STD, 580, 275,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15371, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-1,   9, STD, 580, 300,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
    ENDCASE    
    CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-1,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-1,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
    ENDCASE

    ;*****************************************
    ; Block 2 Tab
    ;*****************************************
  TABPAGE, 3083, 3074, 1, 3, NOTIMP, " Block 2 "

   STATIC, 1, BLOCK-CHARGE,  0, BLOCKS-ARE, 0, 0, 0, 30, 30, -1, STD, LEFT, "Energy Block Format:   ", "", 0, 3
   COMBO, 12306, 12499, 0, 1, BLOCK-CHARGE, 0, BLOCK2-TYPE,  0, STD, 110,  75, 200, 160, 19, 3,  "Block Type:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Type of block calculation; specifies the basis of block charges for this block"
    
    CASE,  BLOCK-CHARGE,  0, BLOCK2-TYPE,  -1,  =, 1, 1
       CASE,  BLOCK-CHARGE,  0, BLOCKS-ARE,  -1,  =, 1, 1
         LABEL, "Cumulative Limit",   STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "(block type unit)",  STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE     
       CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE
    ENDCASE    
    CASE, BLOCK-CHARGE, 0, BLOCK2-TYPE, -1, =, 2, 2, 3
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"

         LABEL, "Limit (block",  STD, CENTER, 623,  42, 1, 0, 0,   0, 15362, 3
         LABEL, "type unit)",    STD, CENTER, 623,  58, 1, 0, 0,   0, 15362, 3
          EDIT, 15362, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   0, STD, 580,  75,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15363, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   1, STD, 580, 100,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15364, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   2, STD, 580, 125,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15365, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   3, STD, 580, 150,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15366, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   4, STD, 580, 175,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15367, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   5, STD, 580, 200,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15368, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   6, STD, 580, 225,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15369, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   7, STD, 580, 250,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15370, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   8, STD, 580, 275,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15371, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-2,   9, STD, 580, 300,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
    ENDCASE    
    CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-2,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-2,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
    ENDCASE

    ;*****************************************
    ; Block 3 Tab
    ;*****************************************
  TABPAGE, 3084, 3074, 1, 3, NOTIMP, " Block 3 "

   STATIC, 1, BLOCK-CHARGE,  0, BLOCKS-ARE, 0, 0, 0, 30, 30, -1, STD, LEFT, "Energy Block Format:   ", "", 0, 3
   COMBO, 12309, 12499, 0, 1, BLOCK-CHARGE, 0, BLOCK3-TYPE,  0, STD, 110,  75, 200, 160, 19, 3,  "Block Type:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Type of block calculation; specifies the basis of block charges for this block"
    
    CASE,  BLOCK-CHARGE,  0, BLOCK3-TYPE,  -1,  =, 1, 1
       CASE,  BLOCK-CHARGE,  0, BLOCKS-ARE,  -1,  =, 1, 1
         LABEL, "Cumulative Limit",   STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "(block type unit)",  STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE     
       CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE
    ENDCASE    
    CASE, BLOCK-CHARGE, 0, BLOCK3-TYPE, -1, =, 2, 2, 3
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"

         LABEL, "Limit (block",  STD, CENTER, 623,  42, 1, 0, 0,   0, 15362, 3
         LABEL, "type unit)",    STD, CENTER, 623,  58, 1, 0, 0,   0, 15362, 3
          EDIT, 15362, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   0, STD, 580,  75,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15363, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   1, STD, 580, 100,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15364, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   2, STD, 580, 125,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15365, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   3, STD, 580, 150,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15366, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   4, STD, 580, 175,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15367, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   5, STD, 580, 200,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15368, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   6, STD, 580, 225,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15369, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   7, STD, 580, 250,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15370, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   8, STD, 580, 275,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15371, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-3,   9, STD, 580, 300,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
    ENDCASE    
    CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-3,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-3,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
    ENDCASE

    ;*****************************************
    ; Block 4 Tab
    ;*****************************************
  TABPAGE, 3085, 3074, 1, 3, NOTIMP, " Block 4 "

   STATIC, 1, BLOCK-CHARGE,  0, BLOCKS-ARE, 0, 0, 0, 30, 30, -1, STD, LEFT, "Energy Block Format:   ", "", 0, 3
   COMBO, 12312, 12499, 0, 1, BLOCK-CHARGE, 0, BLOCK4-TYPE,  0, STD, 110,  75, 200, 160, 19, 3,  "Block Type:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Type of block calculation; specifies the basis of block charges for this block"
    
    CASE,  BLOCK-CHARGE,  0, BLOCK4-TYPE,  -1,  =, 1, 1
       CASE,  BLOCK-CHARGE,  0, BLOCKS-ARE,  -1,  =, 1, 1
         LABEL, "Cumulative Limit",   STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "(block type unit)",  STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE     
       CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE
    ENDCASE    
    CASE, BLOCK-CHARGE, 0, BLOCK4-TYPE, -1, =, 2, 2, 3
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"

         LABEL, "Limit (block",  STD, CENTER, 623,  42, 1, 0, 0,   0, 15362, 3
         LABEL, "type unit)",    STD, CENTER, 623,  58, 1, 0, 0,   0, 15362, 3
          EDIT, 15362, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   0, STD, 580,  75,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15363, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   1, STD, 580, 100,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15364, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   2, STD, 580, 125,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15365, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   3, STD, 580, 150,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15366, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   4, STD, 580, 175,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15367, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   5, STD, 580, 200,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15368, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   6, STD, 580, 225,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15369, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   7, STD, 580, 250,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15370, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   8, STD, 580, 275,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15371, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-4,   9, STD, 580, 300,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
    ENDCASE    
    CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-4,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-4,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
    ENDCASE

    ;*****************************************
    ; Block 5 Tab
    ;*****************************************
  TABPAGE, 3086, 3074, 1, 3, NOTIMP, " Block 5 "

   STATIC, 1, BLOCK-CHARGE,  0, BLOCKS-ARE, 0, 0, 0, 30, 30, -1, STD, LEFT, "Energy Block Format:   ", "", 0, 3
   COMBO, 12315, 12499, 0, 1, BLOCK-CHARGE, 0, BLOCK5-TYPE,  0, STD, 110,  75, 200, 160, 19, 3,  "Block Type:",  LEFT,  -80, 5, 0, LEFT, 4, 5, "Type of block calculation; specifies the basis of block charges for this block"
    
    CASE,  BLOCK-CHARGE,  0, BLOCK5-TYPE,  -1,  =, 1, 1
       CASE,  BLOCK-CHARGE,  0, BLOCKS-ARE,  -1,  =, 1, 1
         LABEL, "Cumulative Limit",   STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "(block type unit)",  STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11538, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE     
       CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
       ENDCASE
    ENDCASE    
    CASE, BLOCK-CHARGE, 0, BLOCK5-TYPE, -1, =, 2, 2, 3
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"

         LABEL, "Limit (block",  STD, CENTER, 623,  42, 1, 0, 0,   0, 15362, 3
         LABEL, "type unit)",    STD, CENTER, 623,  58, 1, 0, 0,   0, 15362, 3
          EDIT, 15362, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   0, STD, 580,  75,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15363, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   1, STD, 580, 100,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15364, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   2, STD, 580, 125,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15365, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   3, STD, 580, 150,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15366, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   4, STD, 580, 175,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15367, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   5, STD, 580, 200,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15368, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   6, STD, 580, 225,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15369, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   7, STD, 580, 250,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15370, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   8, STD, 580, 275,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
          EDIT, 15371, 11539, 0, 1, BLOCK-CHARGE,  0,  LIMITS-5,   9, STD, 580, 300,  23,  90,  2, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Maximum limit for this block (if Block Type is KWH/KW or KWH/KW-Limitsum); 0=no limit"
    ENDCASE    
    CASE, ELSE
         LABEL, "Step Size (block",  STD, CENTER, 422,  42, 1, 0, 0,   0, 15342, 3
         LABEL, "type unit)",        STD, CENTER, 422,  58, 1, 0, 0,   0, 15342, 3
          EDIT, 15342, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   0, STD, 380,  75,  23,  90,  2, 3,  "Step 1:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15343, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   1, STD, 380, 100,  23,  90,  2, 3,  "Step 2:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15344, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   2, STD, 380, 125,  23,  90,  2, 3,  "Step 3:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15345, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   3, STD, 380, 150,  23,  90,  2, 3,  "Step 4:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15346, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   4, STD, 380, 175,  23,  90,  2, 3,  "Step 5:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15347, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   5, STD, 380, 200,  23,  90,  2, 3,  "Step 6:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15348, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   6, STD, 380, 225,  23,  90,  2, 3,  "Step 7:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15349, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   7, STD, 380, 250,  23,  90,  2, 3,  "Step 8:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15350, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   8, STD, 380, 275,  23,  90,  2, 3,  "Step 9:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"
          EDIT, 15351, 11541, 0, 1, BLOCK-CHARGE,  0,  BLOCKS-5,   9, STD, 380, 300,  23,  90,  2, 3, "Step 10:",   LEFT,  -55, 5, 1, LEFT, 4, 5, "The step size of the block (same units as the block Type); maximum of ten"

         LABEL, "Rate ($/block",  STD, CENTER, 523,  42, 1, 0, 0,   0, 15352, 3
         LABEL, "type unit)",     STD, CENTER, 523,  58, 1, 0, 0,   0, 15352, 3
          EDIT, 15352, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   0, STD, 480,  75,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15353, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   1, STD, 480, 100,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15354, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   2, STD, 480, 125,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15355, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   3, STD, 480, 150,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15356, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   4, STD, 480, 175,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15357, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   5, STD, 480, 200,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15358, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   6, STD, 480, 225,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15359, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   7, STD, 480, 250,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15360, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   8, STD, 480, 275,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
          EDIT, 15361, 11540, 0, 1, BLOCK-CHARGE,  0,   COSTS-5,   9, STD, 480, 300,  23,  90,  6, 3,         "",   LEFT,   -2, 5, 1, LEFT, 4, 5, "Cost per unit for the energy or demand falling within this block"
    ENDCASE



 ;********************************************************************
 ;********************************************************************
 ;**
 ;**		Demand Ratchet Data Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************
MODTABDLG, 3199, 3075, 1, 100, 100, 470, 710, 0, RATCHET, "Demand Ratchet Properties", NOTIMP, 0, NOTIMP, 0 
    
   COMBO, 12500, 12500, 0, 1, RATCHET, 0, NAME,  0, STD, 215,  15, 400, 250, 19, 3, "Currently Active Demand Ratchet:",  LEFT, -200, 5, 0, LEFT, 4, 5, "List of all demand ratchets defined in project; also allows library retrieval and creation"
    
    ;*****************************************
    ; Basic Specifications Tab
    ;*****************************************
  TABPAGE, 3200, 3075, 1, 3, NOTIMP, " Basic Specifications "

    EDIT, 12501, 12501, 0, 1, RATCHET, 0,        NAME,  0, STD, 170,  10,  23, 250, 32, 3,  "Demand Ratchet Name:",  LEFT, -150, 5, 1, LEFT, 4, 5, "Name of demand ratchet; right mouse quick menu options allow deleting, copying, linking and saving to library"
    EDIT, 12502, 12502, 0, 1, RATCHET, 0,  NUM-MONTHS,  0, STD, 170,  75,  23,  60,  0, 3,     "Number of Months:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Period over which current ratchet is calculated (1 = current month only)"
   COMBO, 12503, 12503, 0, 1, RATCHET, 0,        TYPE,  0, STD, 170, 100, 300, 160, 19, 3,         "Ratchet Type:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Whether demand is based on the highest monthly peak or average monthly peak"
    EDIT, 12265, 12265, 0, 1, RATCHET, 0,      OFFSET,  0, STD, 170, 125,  23,  60,  2, 3,       "Ratchet Offset:",  LEFT, -150, 5, 1, LEFT, 4, 5, "A number added to the demand (demand + Offest is not allowed to fall below zero)"
    EDIT, 12587, 12587, 0, 1, RATCHET, 0,    FRACTION,  0, STD, 170, 150,  23,  60,  3, 3,     "Ratchet Fraction:",  LEFT, -150, 5, 1, LEFT, 4, 5, "A number between 0 and 1 that is multiplied against the demand"
   COMBO, 12727, 12727, 0, 1, RATCHET, 0, RATCHET-SCH,  0, STD, 170, 175, 200, 160, 19, 3,     "Ratchet Schedule:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Name of a schedule that defines the period over which the ratchet is calculated"
    EDIT, 12728, 12728, 0, 1, RATCHET, 0,    SCH-FLAG,  0, STD, 170, 200,  23,  60,  2, 3,  "Schedule Flag Value:",  LEFT, -150, 5, 0, LEFT, 4, 5, "Flag value in the Ratchet Schedule that indicates when this ratchet is active"

;TO DO !!!
;  BUTTON,     8, 8, 0, 0,    1, STD, 105, 290, 24, 90, 3, "Default", "" 	
;  BUTTON,     1, 1, 0, 1,    1, STD, 205, 290, 24, 90, 3, "OK", "" 	
;  BUTTON,     2, 2, 0, 0,    2, STD, 305, 290, 24, 90, 3, "Cancel", "" 	


 
 ;********************************************************************
 ;********************************************************************
 ;**
 ;**		Life Cycle Cost Tab Dialog
 ;**
 ;********************************************************************
 ;********************************************************************
MODTABDLG, 3113,  32080, 1, 100, 100, 470, 710, 0, NOTIMP, "Life Cycle Cost Properties", NOTIMP, 0, NOTIMP, 0 
 
  ;******************************************************
  ; Baseline Tab
  ;******************************************************
   TABPAGE, 3114, 32087, 1, 3, BASELINE, " Baseline Data "
 
    LABEL, "Utility and Operations Costs", STD, LEFT, 30, 20, 1, 0, 0, 330, 11604, 3
   SPREAD, 11604, 11604, 0, 1, 0, PowerDOE, 0, Baseline, 0, STD, 30, 38, 370, 300, 19, 3, "", LEFT, 0, 0, 0, LEFT, 0, 0, ""

    LABEL, "First Cost and Replacement Costs", STD, LEFT, 405, 20, 1, 0, 0, 670, 14147, 3
     EDIT, 14147, 14147, 0, 1, BASELINE, 0,          FIRST-COST,  0, STD,  540,  35,  23, 100, 2, 3,          "First Cost:",   LEFT, -120, 5, 1, LEFT, 4, 5, "Total baseline initial costs, including installation (zero for existing, unmodified buildings)"
     EDIT, 14148, 14148, 0, 1, BASELINE, 0,        REPLACE-COST,  0, STD,  540,  60,  23, 100, 2, 3,        "Replace Cost:",   LEFT, -120, 5, 1, LEFT, 4, 5, "Present value of the life-cycle baseline replacement costs"
   
    LABEL, "Discount and Inflation Rates", STD, LEFT, 405, 120, 1, 0, 0, 670, 14151, 3
     EDIT, 14151, 14151, 0, 1, BASELINE, 0,       DISCOUNT-RATE,  0, STD,  580, 135,  23,  60, 2, 3,       "Discount Rate:",   LEFT, -160, 5, 1, LEFT, 4, 5, "The discount rate that DOE-2 uses in the life-cycle cost calculations"
     EDIT, 14152, 14152, 0, 1, BASELINE, 0,        LABOR-INFLTN,  0, STD,  580, 160,  23,  60, 2, 3,     "Labor Inflation:",   LEFT, -160, 5, 1, LEFT, 4, 5, "Annual % increase in labor costs (above the inflation rate), applies to maintenance labor only"
     EDIT, 14153, 14153, 0, 1, BASELINE, 0,    MATERIALS-INFLTN,  0, STD,  580, 185,  23,  60, 2, 3, "Materials Inflation:",   LEFT, -160, 5, 1, LEFT, 4, 5, "Annual % increase in materials costs (above inflation), applies to non-maintenance labor also"

    LABEL, "Other Parameters", STD, LEFT, 405, 245, 1, 0, 0, 670, 14154, 3
     EDIT, 14154, 14154, 0, 1, BASELINE, 0,        PROJECT-LIFE,  0, STD,  580, 260,  23,  60, 2, 3,        "Project Life:",   LEFT, -160, 5, 1, LEFT, 4, 5, "Period of time over which DOE-2 calculates life-cycle costs"
     EDIT, 14155, 14155, 0, 1, BASELINE, 0,               LABOR,  0, STD,  580, 285,  23,  60, 2, 3,               "Labor:",   LEFT, -160, 5, 1, LEFT, 4, 5, "Cost of maintenance labor, in dollars per hour"
     EDIT, 14156, 14156, 0, 1, BASELINE, 0,         SITE-FACTOR,  0, STD,  580, 310,  23,  60, 2, 3,         "Site Factor:",   LEFT, -160, 5, 1, LEFT, 4, 5, "Multiplier on the Maintenance and Consumables costs (for different locations in a siting)"
     EDIT, 14149, 14149, 0, 1, BASELINE, 0,     ENERGY-USE-SITE,  0, STD,  540, 335,  23, 100, 2, 3,     "Site Energy Use:",   LEFT, -120, 5, 1, LEFT, 4, 5, "Baseline annual energy use at the site (i.e., at the building boundary)"
     EDIT, 14150, 14150, 0, 1, BASELINE, 0,      ENERGY-USE-SRC,  0, STD,  540, 360,  23, 100, 2, 3,   "Source Energy Use:",   LEFT, -120, 5, 1, LEFT, 4, 5, "Baseline source annual energy use: Site Energy use divided by (transmission) loss fraction"
 
  ;******************************************************
  ; Central Plant Component Costs Tab
  ;******************************************************
   TABPAGE, 3115, 3115, 1, 3, MATERIALS-COST, " Central Plant Component Costs "
   
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;
; CONVERSION STEPS:
;
; 1. Add BDL Command Edited (or NOTIMP) before Caption for dialogs, tabbed dialogs & tabbed dialog pages
;
; 2. Change tabbed dialog size from "310, 610" to "470, 710"
;
; 3. Change label and units label coordinates to be in relation to top-left and top-right corners of the control
;
; 4. Add two properties to each LABEL -> right shadowline X coord & ID of associated UI control (both 0 for none)
;    - also remove trailing ':'s from labels with shadowline extensions
;
; 5. Switch all ComboBox "Height of edit portion of control" values from 21 to 19
;
; 6. Switch all Edit "Height" values from 21 to 23
;
; 7. Switch all font settings of "ITALIC_UND" to "STD"
;
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 
;xxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxxx 

   COMBO, 14221, 14221, 0, 1, MATERIALS-COST, 0, NAME, 0, STD, 360,  10, 350, 220, 19, 3, "Currently Active Central Plant Component Cost:", RIGHT, -10, 5, 0, LEFT, 4, 5, "List of all materials cost components defined in project; also allows library retrieval and creation"
    LINE, 20, 50, 685, 50, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
    
    EDIT, 14222, 14222, 0, 1, MATERIALS-COST, 0, NAME,             0, STD, 155,  85,  23, 220, 32, 3,   "Component Name:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Name of the materials cost component; right mouse quick menu options allow deleting, copying, linking and saving to library"
;  COMBO, 14222, 14222, 0, 1, MATERIALS-COST, 0, NAMEOPT,          0, STD, 145,  60, 136, 150, 21, 3,   "Component Name:",  LEFT,  10, 5, 0, LEFT, 4, 5, "List of all materials costs defined in project; also allows library retrieval"

   LABEL, "Cost Parameters", STD, LEFT, 40, 133, 1, 0, 0, 305, 14223, 3
    EDIT, 14223, 14223, 0, 1, MATERIALS-COST, 0,      FIRST-COST,  0, STD, 185, 150,  23, 100,  2, 3,              "First Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, "First cost for one piece of equipment, not including installation costs"
    EDIT, 14224, 14224, 0, 1, MATERIALS-COST, 0,    INSTALLATION,  0, STD, 185, 175,  23, 100,  2, 3,       "Installation Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, "A multiplier applied to First Cost to obtain the total installation cost per unit"
    EDIT, 14225, 14225, 0, 1, MATERIALS-COST, 0, MINOR-OVHL-COST,  0, STD, 185, 200,  23, 100,  2, 3,     "Minor Overhaul Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Cost for a minor overhaul (must correspond to Minor Overhaul Interval)"
    EDIT, 14226, 14226, 0, 1, MATERIALS-COST, 0, MAJOR-OVHL-COST,  0, STD, 185, 225,  23, 100,  2, 3,     "Major Overhaul Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Cost for a major overhaul (must correspond to Major Overhaul Interval)"
    EDIT, 14227, 14227, 0, 1, MATERIALS-COST, 0,     CONSUMABLES,  0, STD, 185, 250,  23, 100,  2, 3,             "Consumables:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Cost of materials consumed during operation, excluding primary fuel ($/unit/hour)"
   
   LABEL, "Time Parameters", STD, LEFT, 385, 133, 1, 0, 0, 665, 14228, 3
    EDIT, 14228, 14228, 0, 1, MATERIALS-COST, 0,  EQUIPMENT-LIFE,  0, STD, 545, 150,  23, 100,  2, 3,          "Equipment Life:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Number of operating hours after which the unit must be replaced"
    EDIT, 14229, 14229, 0, 1, MATERIALS-COST, 0,      HOURS-USED,  0, STD, 545, 175,  23, 100,  2, 3,              "Hours Used:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Number of hours that existing equipment has already operated (before analysis)"
    EDIT, 14230, 14230, 0, 1, MATERIALS-COST, 0,  MINOR-OVHL-INT,  0, STD, 545, 200,  23, 100,  2, 3, "Minor Overhaul Interval:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Expected operating hours between minor overhauls (must correspond to Minor Overhaul Cost)"
    EDIT, 14231, 14231, 0, 1, MATERIALS-COST, 0,  MAJOR-OVHL-INT,  0, STD, 545, 225,  23, 100,  2, 3, "Major Overhaul Interval:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Expected operating hours between major overhauls (must correspond to Major Overhaul Cost)"
    EDIT, 14232, 14232, 0, 1, MATERIALS-COST, 0,     MAINTENANCE,  0, STD, 545, 250,  23, 100,  2, 3,             "Maintenance:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Number of hours per year of maintenance that each piece of equipment requires"

  ;******************************************************
  ; Other Building Component Costs Tab
  ;******************************************************
   TABPAGE, 3116, 3116, 1, 3, COMPONENT-COST, " Other Building Component Costs "

   COMBO, 14233, 14233, 0, 1, COMPONENT-COST, 0, NAME, 0, STD, 355,  10, 350, 220, 19, 3, "Currently Active Building Component Cost:", RIGHT, -10, 5, 0, LEFT, 4, 5, "List of all component cost components defined in project; also allows library retrieval and creation"
    LINE, 20, 50, 685, 50, -1, SOLID, 128, 128, 128, THIN, 1, 0, 0, 3
    
    EDIT, 14234, 14234, 0, 1, COMPONENT-COST, 0, NAME,             0, STD, 155,  85,  23, 220, 32, 3,   "Component Name:",  LEFT, -115, 5, 1, LEFT, 4, 5, "Name of the component cost component; right mouse quick menu options allow deleting, copying, linking and saving to library"
;  COMBO, 14234, 14234, 0, 1, COMPONENT-COST, 0, NAMEOPT,          0, STD,  145,  60, 136, 150, 21, 3,          "Component Name:",  LEFT,  10, 5, 0, LEFT, 4, 5, "List of all component costs defined in project; also allows library retrieval"

   LABEL, "Unit Description", STD, LEFT, 40, 133, 1, 0, 0, 305, 0, 3
    EDIT, 14245, 14245, 0, 1, COMPONENT-COST, 0,       UNIT-NAME, -1, STD, 150, 150,  23, 135, 16, 3,               "Unit Name:",  LEFT,  -95, 5, 0, LEFT, 4, 5, "Description of the type of building material that this set of component costs applies to"
    EDIT, 14246, 14246, 0, 1, COMPONENT-COST, 0, NUMBER-OF-UNITS,  0, STD, 185, 175,  23, 100,  2, 3,         "Number of Units:",  LEFT, -130, 5, 1, LEFT, 4, 5, "A multiplier on all of the costs (for this set of component costs)"

   LABEL, "Cost Parameters", STD, LEFT, 40, 223, 1, 0, 0, 305, 14235, 3
    EDIT, 14235, 14235, 0, 1, COMPONENT-COST, 0,      FIRST-COST,  0, STD, 185, 240,  23, 100,  2, 3,              "First Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Initial cost per unit (see Number of Units), excluding installation costs"
    EDIT, 14236, 14236, 0, 1, COMPONENT-COST, 0,    INSTALL-COST,  0, STD, 185, 265,  23, 100,  2, 3,       "Installation Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Installation cost per unit, excluding the First Cost"
    EDIT, 14239, 14239, 0, 1, COMPONENT-COST, 0,     ANNUAL-COST,  0, STD, 185, 290,  23, 100,  2, 3,             "Annual Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Annual maintenance (labor) and consumables (materials) cost per unit"
    EDIT, 14237, 14237, 0, 1, COMPONENT-COST, 0,   MIN-OVHL-COST,  0, STD, 185, 315,  23, 100,  2, 3,     "Minor Overhaul Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Cost of a minor overhaul, per unit "
    EDIT, 14238, 14238, 0, 1, COMPONENT-COST, 0,   MAJ-OVHL-COST,  0, STD, 185, 340,  23, 100,  2, 3,     "Major Overhaul Cost:",  LEFT, -130, 5, 1, LEFT, 4, 5, "Cost of a major overhaul, per unit "
  
   LABEL, "Time Parameters", STD, LEFT, 385, 223, 1, 0, 0, 665, 14240, 3
    EDIT, 14240, 14240, 0, 1, COMPONENT-COST, 0,  COMPONENT-LIFE,  0, STD, 545, 240,  23, 100,  2, 3,          "Component Life:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Expected life of the component: i.e., frequency that First- & Installation-Costs are incurred"
    EDIT, 14242, 14242, 0, 1, COMPONENT-COST, 0,    MIN-OVHL-INT,  0, STD, 545, 265,  23, 100,  2, 3, "Minor Overhaul Interval:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Expected time between minor overhauls, i.e frequency Minor Overhaul Costs are incurred"
    EDIT, 14243, 14243, 0, 1, COMPONENT-COST, 0,    MAJ-OVHL-INT,  0, STD, 545, 290,  23, 100,  2, 3, "Major Overhaul Interval:",  LEFT, -145, 5, 1, LEFT, 4, 5, "Expected time between minor overhauls, i.e frequency Major Overhaul Costs are incurred"



 ;********************************************************************
 ;********************************************************************
 ;**
 ;**		Non-Hourly Results Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************

 MODTABDLG, 3142,    0, 1, 30, 30, 280, 505, 0, NOTIMP, "Non-Hourly Results Data", NOTIMP, 0, NOTIMP, 0

   ;*****************************************
   ; Loads Reports
   ;*****************************************
   TABPAGE, 3143,    0, 1, 3, LOADS-REPORT, " Loads Reports "

     SPREAD, 11508, 11508, 0, 1, 0, PowerDOE,         0, NHLoadsSpread,      0, STD,     20,  20, 130, 460, 19, 3, "",                         LEFT,  0,   0, 0, LEFT, 0, 0, "non-hourly loads reports"

     COMBO,  14805, 14805, 0, 1,    LOADS-REPORT,     0, REPORT-FREQUENCY,   0, STD,    182, 160, 120, 100, 19, 3, "Report Frequency:",        LEFT, -162, 5, 0, LEFT, 0, 0, ""
     COMBO,  14806, 14806, 0, 1,    LOADS-REPORT,     0, HOURLY-DATA-SAVE,   0, STD,    182, 185, 120, 100, 19, 3, "Hourly Data Save Format:", LEFT, -162, 5, 0, LEFT, 0, 0, ""

     SPREAD, 11680, 11680, 0, 1, 0, PowerDOE,         0, NHDumpLoadsSpread,  0, STD,    340, 160,  80, 140, 19, 3, "",                         LEFT,  0,   0, 0, LEFT, 0, 0, "non-hourly loads report dump options"
    
   ;*****************************************
   ; System Reports
   ;*****************************************
   TABPAGE, 3144,     0, 1, 3, SYSTEMS-REPORT, " System Reports "

     SPREAD, 11509, 11509, 0, 1, 0, PowerDOE,         0, NHSysSpread,        0, STD,     20,  20, 120, 460, 19, 3, "",                         LEFT,  0,   0, 0, LEFT, 0, 0, "non-hourly system reports"

     COMBO,  14807, 14807, 0, 1,    SYSTEMS-REPORT,   0, REPORT-FREQUENCY,   0, STD,    182, 160, 120, 100, 19, 3, "Report Frequency:",        LEFT, -162, 5, 0, LEFT, 0, 0, ""
     COMBO,  14808, 14808, 0, 1,    SYSTEMS-REPORT,   0, HOURLY-DATA-SAVE,   0, STD,    182, 185, 120, 100, 19, 3, "Hourly Data Save Format:", LEFT, -162, 5, 0, LEFT, 0, 0, ""

     SPREAD, 11681, 11681, 0, 1, 0, PowerDOE,         0, NHDumpSysSpread,    0, STD,    340, 160,  80, 140, 19, 3, "",                         LEFT,  0,   0, 0, LEFT, 0, 0, "non-hourly system report dump options"
    
   ;*****************************************
   ; Plant Reports
   ;*****************************************
   TABPAGE, 3145,     0, 1, 3, PLANT-REPORT, " Plant Reports "

     SPREAD, 11510, 11510, 0, 1, 0, PowerDOE,         0, NHPlantSpread,      0, STD,     20,  20, 120, 460, 19, 3, "",                         LEFT,  0,   0, 0, LEFT, 0, 0, "non-hourly plant reports"

     COMBO,  14809, 14809, 0, 1,    PLANT-REPORT,     0, REPORT-FREQUENCY,   0, STD,    182, 160, 120, 100, 19, 3, "Report Frequency:",        LEFT, -162, 5, 0, LEFT, 0, 0, ""
     COMBO,  14810, 14810, 0, 1,    PLANT-REPORT,     0, HOURLY-DATA-SAVE,   0, STD,    182, 185, 120, 100, 19, 3, "Hourly Data Save Format:", LEFT, -162, 5, 0, LEFT, 0, 0, ""

     SPREAD, 11682, 11682, 0, 1, 0, PowerDOE,         0, NHDumpPlantSpread,  0, STD,    340, 160,  80, 140, 19, 3, "",                         LEFT,  0,   0, 0, LEFT, 0, 0, "non-hourly plant report dump options"
    
   ;*****************************************
   ; Economic Reports
   ;*****************************************
   TABPAGE, 3146,     0, 1, 3, ECONOMICS-REPORT, " Economics Reports "

     SPREAD, 11511, 11511, 0, 1, 0, PowerDOE,         0, NHEconSpread,       0, STD,     20,  20, 120, 460, 19, 3, "",                         LEFT,  0,   0, 0, LEFT, 0, 0, "non-hourly economics reports"

     COMBO,  14811, 14811, 0, 1,    ECONOMICS-REPORT, 0, REPORT-FREQUENCY,   0, STD,    182, 160, 120, 100, 19, 3, "Report Frequency:",        LEFT, -162, 5, 0, LEFT, 0, 0, ""
     COMBO,  14812, 14812, 0, 1,    ECONOMICS-REPORT, 0, HOURLY-DATA-SAVE,   0, STD,    182, 185, 120, 100, 19, 3, "Hourly Data Save Format:", LEFT, -162, 5, 0, LEFT, 0, 0, ""

     SPREAD, 11683, 11683, 0, 1, 0, PowerDOE,         0, NHDumpEconSpread,   0, STD,    340, 160,  80, 140, 19, 3, "",                         LEFT,  0,   0, 0, LEFT, 0, 0, "non-hourly economics report dump options"



 ;********************************************************************
 ;********************************************************************
 ;**
 ;**		Compliance Tabbed Dialog
 ;**
 ;********************************************************************
 ;********************************************************************

; SAC 10/23/00 - Compliance command
MODTABDLG, 3221,    0, 1, 100, 100, 470, 710, 0, COMPLIANCE, "Compliance Analysis Data", NOTIMP, 0, NOTIMP, 0

    ;*****************************************
    ; Basic Specifications Tab
    ;*****************************************
; AFR 6/18/09 - changed the compliance flag from 1 => 7 ... any ruleset loaded that is not LEED.    
  TABPAGE, 3222,    0, 1, 7, NOTIMP, " Basic Specifications "

    EDIT, 15419, 15419, 0, 1, COMPLIANCE, 0,        NAME,  0, STD, 215,  10,  23, 250, 32, 3,  "Compliance Component Name:",  LEFT, -185, 5, 1, LEFT, 4, 5, "Name of this compliance analysis data component"

   LABEL, "Compliance Analysis Data", STD, LEFT, 30, 60, 1, 0, 0, 680, 15420, 1
   COMBO,    15420, 15420, 0, 1, COMPLIANCE, 0,   C-PERMIT-SCOPE, -1, STD, 140,  80, 300, 200, 19, 1,  "Permit Scope:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "The scope of the permit for this project"
   COMBO,    15421, 15421, 0, 1, COMPLIANCE, 0,     C-CONS-PHASE, -1, STD, 140, 105, 300, 200, 19, 1,   "Cons. Phase:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "The phase of construction for this project"
    EDIT,    15422, 15422, 0, 1, COMPLIANCE, 0,  C-DATE-OF-PLANS, -1, STD, 140, 130,  23, 200, 32, 1, "Date of Plans:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "The date on the construction documents used as the basis for this compliance documentation"

   COMBO,    15423, 15423, 0, 1, COMPLIANCE, 0,  C-BUILDING-TYPE, -1, STD, 450,  80, 300, 230, 19, 1, "Building Type:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "The type of building"
    EDIT,    15425, 15425, 0, 1, COMPLIANCE, 0, C-NUM-OF-STORIES, -1, STD, 450, 105,  23, 100,  0, 1,  "Num. Stories:",  LEFT,  -90, 5, 1, LEFT, 4, 5, "The number of above grade floors in this project"
   CHECKBOX, 15424, 15424, 0, 1, COMPLIANCE, 0,    C-NR-DHW-INCL, -1, STD, 451, 133,  17, 190,     1,   "Includes Nonresidential DHW", RIGHT,               "Checked if service/domestic water heating for nonresidential spaces is to be included in the compliance analysis"
   CHECKBOX, 15426, 15426, 0, 1, COMPLIANCE, 0,   C-RES-DHW-INCL, -1, STD, 451, 158,  17, 170,     1,   "Includes Residential DHW",    RIGHT,               "Checked if service/domestic water heating for residential spaces is to be included in the compliance analysis"
;   COMBO,    15425, 15425, 0, 1, COMPLIANCE, 0,   C-RES-DHW-INCL, -1, STD, 450, 155, 300, 230, 19, 1,  "Res DHW Type:",  LEFT,  -90, 5, 0, LEFT, 4, 5, "Select the type of Residential DHW Compliance to be included in the analysis"

; SAC 7/1/03 - Added SBD analysis section and pipe loss toggle and shifted compliance reporting section down by 100
   LABEL, "Savings By Design Analysis Options", STD, LEFT, 30, 205, 1, 0, 0, 680, 0, 4
   CHECKBOX, 17770, 17770, 0, 1, COMPLIANCE, 0, C-COMP-PIPE-LOSS, -1, STD,  50, 225,  18, 230,     4,  "Perform SBD Pipe Loss Analysis",          LEFT,       ""

   LABEL, "Compliance Reporting", STD, LEFT, 30, 305, 1, 0, 0, 680, 15427, 1
    EDIT,    15427, 15427, 0, 1, COMPLIANCE, 0,      C-PROJ-NAME, -1, STD, 190, 325,  23, 490, 76, 1,         "Project Name:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The name of this project"
    EDIT,    15428, 15428, 0, 1, COMPLIANCE, 0,   C-PROJ-ADDRESS, -1, STD, 190, 350,  23, 490, 76, 1,      "Project Address:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The number, street, city, state and zip of this project"
    EDIT,    15429, 15429, 0, 1, COMPLIANCE, 0,    C-DOCU-AUTHOR, -1, STD, 190, 375,  23, 300, 76, 1, "Documentation Author:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The name of the author of the Title 24 compliance documents for this project"
    EDIT,    15430, 15430, 0, 1, COMPLIANCE, 0, C-DOCU-AUTHOR-PH, -1, STD, 560, 375,  23, 120, 32, 1,                "Phone:",  LEFT,  -45, 5, 1, LEFT, 4, 5, "The phone number of the Title 24 compliance document author for this project"

    ;*****************************************
    ; Envelope / Lighting / Mechanical Designers Tab
    ;*****************************************
; AFR 6/18/09 - changed the compliance flag from 1 => 7 ... any ruleset loaded that is not LEED.    
  TABPAGE, 3223,    0, 1, 7, NOTIMP, " Envelope / Lighting / Mechanical "

   LABEL, "Envelope Compliance", STD, LEFT, 30, 40, 1, 0, 0, 680, 15435, 1
    EDIT,    15435, 15435, 0, 1, COMPLIANCE, 0,   C-DESIGNER-ENV, -1, STD, 150,  60,  23, 340, 76, 1,  "Designer Name:",  LEFT, -100, 5, 1, LEFT, 4, 5, "The name of the building envelope designer"
    EDIT,    15436, 15436, 0, 1, COMPLIANCE, 0, C-DESIGNER-PHONE, -1, STD, 560,  60,  23, 120, 32, 1,          "Phone:",  LEFT,  -45, 5, 1, LEFT, 4, 5, "The phone number of the building envelope designer"
    EDIT,    15437, 15437, 0, 1, COMPLIANCE, 0,   C-ENV-MAND-LOC, -1, STD, 380,  85,  23, 300, 76, 1, "Location on plans of Note Block for Mandatory Measures:",  LEFT, -330, 5, 1, LEFT, 4, 5, "The location in the construction documents of the list of envelope mandatory measures"

   LABEL, "Lighting Compliance", STD, LEFT, 30, 140, 1, 0, 0, 680, 15440, 1
    EDIT,    15440, 15440, 0, 1, COMPLIANCE, 0,   C-DESIGNER-LTG, -1, STD, 150, 160,  23, 340, 76, 1,  "Designer Name:",  LEFT, -100, 5, 1, LEFT, 4, 5, "The name of the lighting systems designer for this project"
    EDIT,    15441, 15441, 0, 1, COMPLIANCE, 0,    C-DSNR-LTG-PH, -1, STD, 560, 160,  23, 120, 32, 1,          "Phone:",  LEFT,  -45, 5, 1, LEFT, 4, 5, "The phone number of the lighting systems designer for this project"
    EDIT,    15442, 15442, 0, 1, COMPLIANCE, 0,   C-LTG-MAND-LOC, -1, STD, 380, 185,  23, 300, 76, 1, "Location on plans of Note Block for Mandatory Measures:",  LEFT, -330, 5, 1, LEFT, 4, 5, "The location in the construction documents of the list of lighting mandatory measures"

   LABEL, "Mechanical Compliance", STD, LEFT, 30, 240, 1, 0, 0, 680, 15445, 1
    EDIT,    15445, 15445, 0, 1, COMPLIANCE, 0,  C-DESIGNER-MECH, -1, STD, 150, 260,  23, 340, 76, 1,  "Designer Name:",  LEFT, -100, 5, 1, LEFT, 4, 5, "The name of the mechanical systems designer for this project"
    EDIT,    15446, 15446, 0, 1, COMPLIANCE, 0,   C-DSNR-MECH-PH, -1, STD, 560, 260,  23, 120, 32, 1,          "Phone:",  LEFT,  -45, 5, 1, LEFT, 4, 5, "The phone number of the mechanical systems designer for this project"
    EDIT,    15447, 15447, 0, 1, COMPLIANCE, 0,  C-MECH-MAND-LOC, -1, STD, 380, 285,  23, 300, 76, 1, "Location on plans of Note Block for Mandatory Measures:",  LEFT, -330, 5, 1, LEFT, 4, 5, "The location in the construction documents of the list of mechanical mandatory measures"

;  13> C-RESULT-1                  0         Literal           20  WORDS/ELEMENT =20                126
;  14> C-RESULT-2                  0         Literal           20  WORDS/ELEMENT =20                146
;  15> C-RESULT-3                  0         Literal           20  WORDS/ELEMENT =20                166
;  16> C-RESULT-4                  0         Literal           20  WORDS/ELEMENT =20                186
;  17> C-RESULT-5                  0         Literal           20  WORDS/ELEMENT =20                206


    ;*****************************************
    ; Basic Specifications Tab
    ;*****************************************
; AFR 6/18/09 - added this tab.  This tab will display if the loaded ruleset contains LEED.  The original Basic Spec and
;               Envelope/Lighting/Mechanical tab will display if the compliance flag is set to 7, and loaded ruleset that
;               does not contain LEED.
  TABPAGE, 3226,    0, 1, 6, NOTIMP, " Basic Specifications "

    EDIT, 15431, 15419, 0, 1, COMPLIANCE, 0,        NAME,  0, STD, 215,  10,  23, 250, 32, 3,  "Compliance Component Name:",  LEFT, -185, 5, 1, LEFT, 4, 5, "Name of this compliance analysis data component"

   LABEL, "Compliance Analysis Data", STD, LEFT, 30, 60, 1, 0, 0, 680, 15420, 1
   COMBO,    15432, 15423, 0, 1, COMPLIANCE, 0,  C-901-BLDG-TYPE, -1, STD, 148,  80, 300, 200, 19, 1,   "Building Type:",  LEFT,  -98, 5, 0, LEFT, 4, 5, "Predominant ASHREA building type for project"
    EDIT,    15448, 15448, 0, 1, COMPLIANCE, 0,   C-901-NUM-FLRS, -1, STD, 148, 105,  23, 100,  0, 1,     "Num. Floors:",  LEFT,  -98, 5, 1, LEFT, 4, 5, "Number of conditioned floors for project"
   COMBO,    15443, 15443, 0, 1, COMPLIANCE, 0,  C-HTG-SYS-CLASS, -1, STD, 148, 130, 300, 230, 19, 1,  "Heating Source:",  LEFT,  -98, 5, 0, LEFT, 4, 5, "Predominant heating source type for project"


; SAC 7/1/03 - Added SBD analysis section and pipe loss toggle and shifted compliance reporting section down by 100
   LABEL, "Savings By Design Analysis Options", STD, LEFT, 30, 205, 1, 0, 0, 680, 0, 4
   CHECKBOX, 17771, 17770, 0, 1, COMPLIANCE, 0, C-COMP-PIPE-LOSS, -1, STD,  50, 225,  18, 230,     4,  "Perform SBD Pipe Loss Analysis",          LEFT,       ""

   LABEL, "Compliance Reporting", STD, LEFT, 30, 305, 1, 0, 0, 680, 15427, 1
    EDIT,    15438, 15427, 0, 1, COMPLIANCE, 0,      C-PROJ-NAME, -1, STD, 190, 325,  23, 490, 76, 1,         "Project Name:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The name of this project"
    EDIT,    15439, 15428, 0, 1, COMPLIANCE, 0,   C-PROJ-ADDRESS, -1, STD, 190, 350,  23, 490, 76, 1,      "Project Address:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The number, street, city, state and zip of this project"
    EDIT,    15444, 15429, 0, 1, COMPLIANCE, 0,    C-DOCU-AUTHOR, -1, STD, 190, 375,  23, 300, 76, 1, "Documentation Author:",  LEFT, -140, 5, 1, LEFT, 4, 5, "The name of the author of the Title 24 compliance documents for this project"
    EDIT,    15449, 15430, 0, 1, COMPLIANCE, 0, C-DOCU-AUTHOR-PH, -1, STD, 560, 375,  23, 120, 32, 1,                "Phone:",  LEFT,  -45, 5, 1, LEFT, 4, 5, "The phone number of the Title 24 compliance document author for this project"



 ;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Compliance DHW - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************
                          
; SAC 10/23/00 - Compliance command
 MODTABDLG, 3224,    0, 1, 160, 160, 380, 450, 0, COMPLIANCE-DHW, "Residential Dwelling Unit Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   COMBO, 15450, 15450, 0, 1,  COMPLIANCE-DHW,     0,    NAME,  0, STD, 235,  15, 400, 200, 19, 3, "Currently Active Res. Dwelling Unit:", LEFT, -215, 5, 0, LEFT, 4, 5, "This list contains all Holiday sets defined in the project"

    ;******************************************
    ; Compliance DHW - Basic Specs Page
    ;******************************************
    TABPAGE, 3225,    0, 1, 3, NOTIMP, " Basic Specifications "

       EDIT, 15451, 15451, 0, 1,    COMPLIANCE-DHW, 0,         NAME, -1, STD, 155,  10,  23, 225, 32, 3,       "Dwelling Unit Name:",  LEFT, -125,   5, 0, LEFT, 4, 5, "Name of residential dwelling unit"

       EDIT, 15452, 15452, 0, 1,    COMPLIANCE-DHW, 0,  C-NUM-UNITS, -1, STD, 155,  40,  23,  50,  0, 1,          "Number of Units:",  LEFT, -125,   5, 1, LEFT, 4, 5, "The total number of identical residential dwelling units represented by this COMPLIANCE-DHW component"

     SPREAD, 15453, 15453, 0, 1, 0, PowerDOE, 0, CompDHWLoopsSpread,  0, STD, 135,  93, 190, 245, 19, 1, "HW/DHW Circulation Loops:",  LEFT, -105, -18, 0, LEFT, 0, 0, ""

;****************************************************************************************************************
 ;****************************************************************************************************************
 ;**
 ;**     Project Data - Properties Sheet
 ;**
 ;****************************************************************************************************************
 ;****************************************************************************************************************

 MODTABDLG, 3382, 3382, 1, 30, 30, 560, 520, 0, PROJECT-DATA, "Project Data Properties", NOTIMP, 0, NOTIMP, 0

;TO DO: a help item should be added similar to other "Currently Active" help items for other commands
   
    ;******************************************
    ; Project Data - Basic Specs Page
    ;******************************************
    TABPAGE, 3383, 2519, 1, 3, NOTIMP, " Project Data Details "

; TV - Made Row headers tall     SPREAD, 19328, 32079, 0, 1, 0, PowerDOE, 0, ProjectDataSpread,   0, STD,  45, 50, 300, 225, 50, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
; TV - Made Row Headers normal height,but narrow width       SPREAD, 19328, 32079, 0, 1, 0, PowerDOE, 0, ProjectDataSpread,   0, STD,  45, 50, 300, 225, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""
      SPREAD, 19328, 32079, 0, 1, 0, PowerDOE, 0, ProjectDataSpread,   0, STD,  25, 10, 500, 380, 19, 3, "",  LEFT, 0, 0, 0, LEFT, 0, 0, ""


 END



-------------- next part --------------
A non-text attachment was scrubbed...
Name: BDLKEY.BIN
Type: application/octet-stream
Size: 7954160 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200214/db69ff1c/attachment-0002.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: BDLDFT.DAT
Type: application/octet-stream
Size: 1560 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200214/db69ff1c/attachment-0003.obj>


More information about the Equest-users mailing list