[Equest-users] eQuest Infiltration Modeling as Airflow (CFM/ft2)
Nicholas Caton
Nicholas.Caton at se.com
Mon Dec 28 19:13:48 PST 2020
Well stated Brian!
An extra anecdote/caution:
Brian’s sentiment expressed here – that pressures typical of blower door testing for envelope leakage are atypical for those found caused naturally through wind pressures and other forces for infiltration/exfiltration, is correct. Most of the time.
If however you are tuning a model expressly to evaluate measures specifically affecting infiltration, be mindful that nature likes to play outside the box sometimes. I was tuning a specific laboratory building with extremely leaky glazing (partly because the building was a mechanical vacuum cleaner, mostly because the glazing was original to the building, nearly 70 years old), and was utilizing AMY weather to assist with a particularly weather-sensitive and touchy calibration process. That historical weather period coincidentally proved invaluable for this exercise, in part because the calibration period it contained some fairly extreme weather events… Some wacky looking windspeeds in the Spring caused me to google for climactic (?) events in this locality (Illinois), and I found just cause for the resulting extreme external building pressurization/infiltration: tornadoes!
Quick takeaway:
1. While blower door testing is indeed pretty darn extreme in the context of “normal” conditions – nothing is more extreme than mother nature =).
2. This also adds a little perspective on the concerns I hear raised occasionally on the idea that blower door testing with existing/aged facilities can harm with respect to building envelope performance… even if true, it’s nothing in comparison with Midwest weather events of this nature!
~Nick
[cid:image002.jpg at 01D6DDDB.4B28CDF0]
Nick Caton, P.E. (US), BEMP
ニック ケートン, P.E. (US), BEMP
Senior Energy Engineer
Energy Manager, Yokota Airbase
ESS - Energy & Sustainability Services
M JP
M US
Email
+81 . 070 . 3366 . 3317
+1 . 785 . 410 . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
シニアエネルギーエンジニア
横田基地エネルギーマネージャー
ESS - エナジー持続可能性サービス
[cid:image003.png at 01D6DDDB.4B28CDF0]
[cid:image004.png at 01D6DDDB.4B28CDF0]
[cid:image002.jpg at 01D6DDDB.4B28CDF0]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Brian Fountain via Equest-users
Sent: Thursday, December 24, 2020 8:29 AM
To: Omer Moltay <omoltay at mimtarch.com>
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest Infiltration Modeling as Airflow (CFM/ft2)
[External email: Use caution with links and attachments]
________________________________
50 Pa is too high a pressure difference to use for entry into eQUEST – regardless of whether you use ACH or cfm/area. That is a testing pressure differential rather than the ambient pressure differential created by the reference wind speed of 10 mph (4.47 m/s). Ambient wind corresponds to a pressure differential of ~5 Pa. Using the n50 flow rate would considerably overstate your infiltration load.
[cid:image005.png at 01D6D959.0CBDCB50]
(from eQUEST/DOE-2.2 help)
To convert the tested leakage rate (n50) at 50 Pa to the ambient 5 Pa use the formula below …
[cid:image006.png at 01D6D959.0CBDCB50]
Formula taken from an excellent white paper on modelling infiltration by RWDI available here: https://sbcanada.org/wp-content/uploads/2017/04/Air-tightness-Energy-Modelling-for-Part-3-Buildings.pdf<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fsbcanada.org%2Fwp-content%2Fuploads%2F2017%2F04%2FAir-tightness-Energy-Modelling-for-Part-3-Buildings.pdf&data=04%7C01%7CNicholas.Caton%40se.com%7Cd28d7a6799bb44a0242508d8a79a8c2d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637443629515267558%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=yfhNqxEK1TFs9BEcpDWhRH2SIooG8uDkCV1loWkV2ew%3D&reserved=0>
Regards,
Brian
Footprint
Brian Fountain
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Mark Stout via Equest-users
Sent: December 23, 2020 4:03 PM
To: Omer Moltay <omoltay at mimtarch.com<mailto:omoltay at mimtarch.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Spam released by Allowed List] Re: [Equest-users] eQuest Infiltration Modeling as Airflow (CFM/ft2)
CAUTION: EXTERNAL SENDER
I would use ACH and base it on -50 Pa and the standards the AHJ has set. For example, IECC sets some zones to 3 ACH, but the AHJ may/can/do override that and may up it to 5 ACH. Then you just work backwards to arrive at ACH, e.g. the formula for CFM is (5 ACH ÷ 60 Minutes) x Volume = CFM50. Now you know what your max infiltration.
On Wed, Dec 23, 2020 at 12:50 PM Omer Moltay via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
Dear All,
eQuest allows inputing of infiltration airflow as CFM/ft2 (of indoor space in detailed mode) for every zone.
I have calculated CFM/ft2 values for each zone in my model, but this calculation has been done for an outside - inside pressure difference of 50 Pa. Or I can do the calculation for any arbitrary pressure difference.
The question is, since infiltration is very much pressure dependent, what pressure difference does eQuest assume when the infiltration airflow input is utilized? I know that it will not take into account the dynamic changes in pressure dif. during the simulation due to wind effect or other effects, but I just want to be able to input a reasonable value since a calculated infiltration at 50 Pa is very different from say, at 5 Pa. The answer is of course, at whatever pressure difference the zone is anticipated to be operating, so what would you recommend for low-rise commercial buildings? Or any other guidance would be appreciated.
Or should I convert my calculated values to ACH and use that input, as that takes into account wind speed changes? Again, what is the reference pressure dif. to use there?
Thank you,
Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, ASHRAE CPMP
Mimta EcoYapi, LEED Proven Provider
Hekimsuyu Cad. 559. Sk.
No:39 34255 Kucukkoy Istanbul Turkey
Tel: 90-212-617-2296
Fax: 90-212-617-2297
Mobile: 90-533-957-1394
www.eco-yapi.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.eco-yapi.com%2F&data=04%7C01%7CNicholas.Caton%40se.com%7Cd28d7a6799bb44a0242508d8a79a8c2d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637443629515267558%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=30cXHbejkHUiGgsASx9k7DOWrBkTtwAW0qyFAbIhoWE%3D&reserved=0>
www.buildingenergymodels.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.buildingenergymodels.com%2F&data=04%7C01%7CNicholas.Caton%40se.com%7Cd28d7a6799bb44a0242508d8a79a8c2d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637443629515277513%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=0QMI%2BwIH%2FTqSFj68jT5N%2F%2B7mPOFYuUmBFOTVdS2KT2k%3D&reserved=0>
[cid:image001.png at 01D6D955.0DF3FE30]
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=04%7C01%7CNicholas.Caton%40se.com%7Cd28d7a6799bb44a0242508d8a79a8c2d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637443629515277513%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=MPKgvZt3OYK8xlnxQxvl621zC7N%2BeaCw8n%2BK%2BsUcmdU%3D&reserved=0>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Kind Regards,
Mark Stout, President
HERS I & II, BPI BA, MFBA, RESNET HERS
Lighting & Mechanical Acceptance Testing
CALGreen Inspector/Plans Examiner
Apollo Energies, Inc.
888-614-8338 x101 Office
888-614-8338 Fax
916-240-2850 Cell
www.apolloenergiesinc.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.apolloenergiesinc.com%2F&data=04%7C01%7CNicholas.Caton%40se.com%7Cd28d7a6799bb44a0242508d8a79a8c2d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637443629515277513%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=3PWP2Wq%2F7%2F1fTEwpaEEnXnm5%2B6QWJJchmSXV1V5vjKI%3D&reserved=0>
Follow us on Twitter<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ft.sidekickopen70.com%2Fs2t%2Fc%2F5%2Ff18dQhb0S7lC8dDNfKW3w9sL42B9nMJW7t5XZs5vg7Q8W64zSmC5vMHyMW4XXPpC56dL2ff92xgtF02%3Fte%3DW3R5hFj26QkHjW4mCW-d3K8K1pW43T4NQ45SzBFW43PTww49LkxD2273%26si%3D5947551709659136%26pi%3D2aaf2879-36ea-4628-ebdf-95a2ba6101fb&data=04%7C01%7CNicholas.Caton%40se.com%7Cd28d7a6799bb44a0242508d8a79a8c2d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637443629515287470%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=t2t4CdJByYPabsDughiDR5VH%2FJIJNMAOuoAJuja2shA%3D&reserved=0> LinkedIn<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ft.sidekickopen70.com%2Fs2t%2Fc%2F5%2Ff18dQhb0S7lC8dDNfKW3w9sL42B9nMJW7t5XZs5vg7Q8W64zSmC5vMHyMW4XXPpC56dL2ff92xgtF02%3Fte%3DW3R5hFj4cm2zwW4mKLS-3ZWVWBW3K2-zv1JxwY5W1Lw3rh45LM6yW1Gyy403yMFyvw1-X_1g47L2%26si%3D5947551709659136%26pi%3D2aaf2879-36ea-4628-ebdf-95a2ba6101fb&data=04%7C01%7CNicholas.Caton%40se.com%7Cd28d7a6799bb44a0242508d8a79a8c2d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637443629515287470%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=wk0xDVXoGOi%2F61zDyFCzRHnGZs4Tw5N9R1NNrYFVeDo%3D&reserved=0>
Subscribe to Apollo Energies Daily News<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ft.sidekickopen70.com%2Fs2t%2Fc%2F5%2Ff18dQhb0S7lC8dDNfKW3w9sL42B9nMJW7t5XZs5vg7Q8W64zSmC5vMHyMW4XXPpC56dL2ff92xgtF02%3Fte%3DW3R5hFj26QkH0W3zbVbk3H6wfQW4cQb1c45SzBFW43PTww49LkxDW4cKKqL1JxwY51V3%26si%3D5947551709659136%26pi%3D2aaf2879-36ea-4628-ebdf-95a2ba6101fb&data=04%7C01%7CNicholas.Caton%40se.com%7Cd28d7a6799bb44a0242508d8a79a8c2d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637443629515297431%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C2000&sdata=q6ipbe8CMBrftThmML%2FpFlM531KA2tUsgCmB4Lvn9Gw%3D&reserved=0>
DISCLAIMER: I am not an attorney nor am I an accountant. The information and/or opinions expressed by myself or my affiliates should not be considered nor are they intended to provide legal or financial advice to any individual or entity. The information contained in this email is for general information purposes only. Any reliance you place on such information is therefore strictly at your own risk. Apollo Energies Inc., urges you to consult with your own legal and/or financial advisers before taking any further actions based on information provided in this correspondence.
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201229/3017fefc/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1794 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201229/3017fefc/attachment-0003.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 1947 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201229/3017fefc/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 6510 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201229/3017fefc/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 59202 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201229/3017fefc/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 67214 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201229/3017fefc/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 44049 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201229/3017fefc/attachment-0019.png>
More information about the Equest-users
mailing list