[Equest-users] eQuest Infiltration Modeling as Airflow (CFM/ft2)

Mark Stout mark.stout at apolloenergiesinc.com
Wed Dec 23 13:02:45 PST 2020


I would use ACH and base it on -50 Pa and the standards the AHJ has set.
For example, IECC sets some zones to 3 ACH, but the AHJ may/can/do override
that and may up it to 5 ACH.  Then you just work backwards to arrive at
ACH, e.g.  the formula for CFM is (5 ACH  ÷ 60 Minutes) x Volume = CFM50.
Now you know what your max infiltration.


On Wed, Dec 23, 2020 at 12:50 PM Omer Moltay via Equest-users <
equest-users at lists.onebuilding.org> wrote:

> Dear All,
>
> eQuest allows inputing of infiltration airflow as CFM/ft2 (of indoor space
> in detailed mode) for every zone.
>
> I have calculated CFM/ft2 values for each zone in my model, but this
> calculation has been done for a outside - inside pressure difference of 50
> Pa. Or I can do the calculation for any arbitrary pressure difference.
>
> The question is, since infiltration is very much pressure dependent, what
> pressure difference does eQuest assume when the infiltration airflow input
> is utilized? I know that it will not take into account the dynamic changes
> in pressure dif. during the simulation due to wind effect or other effects,
> but I just want to be able to input a reasonable value since a calculated
> infiltration at 50 Pa is very different from say, at 5 Pa. The answer is of
> course, at whatever pressure difference the zone is anticipated to be
> operating, so what would you recommend for low-rise commercial buildings?
> Or any other guidance would be appreciated.
>
> Or should I convert my calculated values to ACH and use that input, as
> that takes into account wind speed changes? Again, what is the reference
> pressure dif. to use there?
>
> Thank you,
>
> Ömer Moltay, LEED AP BD+C, ASHRAE BEMP, ASHRAE CPMP
> Mimta EcoYapi, LEED Proven Provider
> Hekimsuyu Cad. 559. Sk.
> No:39 34255 Kucukkoy Istanbul Turkey
> Tel: 90-212-617-2296
> Fax: 90-212-617-2297
> Mobile: 90-533-957-1394
> www.eco-yapi.com
> www.buildingenergymodels.com
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send  a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>


-- 
Kind Regards,
Mark Stout, President
HERS I & II, BPI BA, MFBA, RESNET HERS
Lighting & Mechanical Acceptance Testing
CALGreen Inspector/Plans Examiner

Apollo Energies, Inc.
888-614-8338 x101 Office
888-614-8338 Fax
916-240-2850 Cell
www.apolloenergiesinc.com
Follow us on Twitter
<https://t.sidekickopen70.com/s2t/c/5/f18dQhb0S7lC8dDNfKW3w9sL42B9nMJW7t5XZs5vg7Q8W64zSmC5vMHyMW4XXPpC56dL2ff92xgtF02?te=W3R5hFj26QkHjW4mCW-d3K8K1pW43T4NQ45SzBFW43PTww49LkxD2273&si=5947551709659136&pi=2aaf2879-36ea-4628-ebdf-95a2ba6101fb>
 LinkedIn
<https://t.sidekickopen70.com/s2t/c/5/f18dQhb0S7lC8dDNfKW3w9sL42B9nMJW7t5XZs5vg7Q8W64zSmC5vMHyMW4XXPpC56dL2ff92xgtF02?te=W3R5hFj4cm2zwW4mKLS-3ZWVWBW3K2-zv1JxwY5W1Lw3rh45LM6yW1Gyy403yMFyvw1-X_1g47L2&si=5947551709659136&pi=2aaf2879-36ea-4628-ebdf-95a2ba6101fb>

Subscribe to Apollo Energies Daily News
<https://t.sidekickopen70.com/s2t/c/5/f18dQhb0S7lC8dDNfKW3w9sL42B9nMJW7t5XZs5vg7Q8W64zSmC5vMHyMW4XXPpC56dL2ff92xgtF02?te=W3R5hFj26QkH0W3zbVbk3H6wfQW4cQb1c45SzBFW43PTww49LkxDW4cKKqL1JxwY51V3&si=5947551709659136&pi=2aaf2879-36ea-4628-ebdf-95a2ba6101fb>



DISCLAIMER:  I am not an attorney nor am I an accountant.  The information
and/or opinions expressed by myself or my affiliates should not be
considered nor are they intended to provide legal or financial advice to
any individual or entity.  The information contained in this email is for
general information purposes only.  Any reliance you place on such
information is therefore strictly at your own risk.  Apollo Energies Inc.,
urges you to consult with your own legal and/or financial advisers before
taking any further actions based on information provided in this
correspondence.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201223/ea9240e0/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 8H1e6MbBxg5EAAAAAAElFTkSuQmCC
Type: image/png
Size: 44049 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20201223/ea9240e0/attachment-0003.png>


More information about the Equest-users mailing list