[Equest-users] eQuest/DOE CHW Thermal Storage kW shift

Nicholas Caton Nicholas.Caton at se.com
Mon Aug 17 09:11:51 PDT 2020


Awesome thread, thanks to both of you!

Daric's heat map and Brian's reaction inspired me to share some related e data visualization efforts I've found helpful over the last year or so.  The combination of pivot tables, time series data, and excel heatmap formatting can be a really useful combination for realizing/identifying patterns and interpreting/understanding complex operations over an extended time period (weeks/months/years...).  Perhaps these examples may serve to help drive the point home for others, allowing you to remember the option when it could help you solve a puzzle:


  1.  For a project featuring real-time variable pricing on the electrical rate (RTP), with no apparent TOU structure, there was a natural temptation to simply determine an annually averaged, marginal rate and use that for projecting the valuation of energy saving measures (ECMs).  However parallel pursuit of solar, roadway lighting upgrades, and other time-of-day sensitive ECM's led me to attempting a "binning" of the historical rates by time of day and season.  In the following pivot, you're seeing a few years' worth of rates averaged by hour of the day (1-24) and by month (1-12).  This heat map formatting helped to reveal consistent jumps and to draw a subjective line between a "day" and "night" rates.  The TOU structure I derived is communicated visually by the thick borders applied across this heatmap:

[cid:image003.png at 01D672CC.424DFB30]

Incidentally, that streak of red values corresponding to the early morning hours of January sparked some deeper dives to understand the root cause of that "deviation."  Turns out there was an odd string of utility outages/incidents which year over year landed in the same calendar periods, resulting in the "spike" seen here... but by all accounts we had no reason to presume that as typical for years to come so I concluded it wasn't appropriate to bin those separately and instead roll those results into the other binned averages.

  1.  As part of a CHP Plant analysis, I needed to answer a number of interrelated questions like "how much power is needed at different times of the day?" and "How often can we get by running fewer than all gensets?"  In a similar fashion, I pivoted a time series of related calculations, again by hour of the day and month of the year (flipped axes from the previous example), to identify seasonal & time-of-day patterns, allowing me to draw conclusions and advise sequencing/maintenance scheduling frameworks:

[cid:image001.png at 01D672E9.74F9C240]

  1.  To take a step away from time-series data, I've also found the combination of pivots + excel conditional formatting helpful for communicating relative benchmarking differences with multiple metrics.  The following example illustrates, for a portfolio of buildings grouped by common occupancy, 3 benchmarking metrics (Total utility spend, EUI, and CUI).  In isolation, these metrics result in different perspectives that would lead someone to different conclusions on where to focus resources/attention.  Taken together, someone can assemble a more nuanced view of where the greatest potential for energy savings may lie:

[cid:image002.png at 01D67487.2F43D570]

[cid:image009.jpg at 01D67487.2F43D570]
Nick Caton, P.E., BEMP
  Senior Energy Engineer
  Energy and Sustainability Services
  Energy Performance Contracting
D
M
E

913 . 564 . 6361
785 . 410 . 3317
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219

[cid:image006.png at 01D672CC.424DFB30]


From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Daric Adair via Equest-users
Sent: Friday, August 14, 2020 9:28 AM
To: Brian Fountain <Brian.Fountain at sa-footprint.com>
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] eQuest/DOE CHW Thermal Storage kW shift


[External email: Use caution with links and attachments]

________________________________


Brian;

Good find on the TES Adjustment variable, I'd missed that. It doesn't appear to have any impact on the bills/rates; but does add a good visibility. Will be useful if we move into excel/hand calc'ing the utility rates for the project. This will either confirm eQuest & complex rates are correct or that something is further wonky...

The Equipment-Control is '-undefined-' due to use of Load-Management sequencing the different Equipment-Control options throughout the year.


Thanks,
DARIC ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst

HENDERSON ENGINEERS<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hendersonengineers.com%2F%3Futm_source%3Dhei%26%26utm_medium%3Demail%26%26utm_campaign%3Dhei-shortsignature&data=02%7C01%7CNicholas.Caton%40se.com%7C7298b25b72204a99255608d8405e56d2%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637330121212948146&sdata=PnC2pZGnoRtHH%2FhzvAmvPp94u5NdzT2hVhLpKGpMgzA%3D&reserved=0>
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>

LICENSED IN KS

HENDERSON PROUD SINCE 1970<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hendersonengineers.com%2Fabout-us%2Four-story%2F%3Futm_source%3Dhei%26utm_medium%3Demail%26utm_campaign%3Dhei-shortsignature&data=02%7C01%7CNicholas.Caton%40se.com%7C7298b25b72204a99255608d8405e56d2%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637330121212958137&sdata=GEyDT31tLK%2BnHeenjlnIhm3aXYlCl%2BXXdlynn0RuEbw%3D&reserved=0> | JUST GETTING STARTED.

From: Brian Fountain <Brian.Fountain at sa-footprint.com<mailto:Brian.Fountain at sa-footprint.com>>
Sent: Friday, August 14, 2020 8:12 AM
To: Daric Adair <Daric.Adair at hendersonengineers.com<mailto:Daric.Adair at hendersonengineers.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: eQuest/DOE CHW Thermal Storage kW shift

Good morning Daric,

Firstly, that is a very slick use of excel to generate a heat map.  Very cool.

I believe the answer to your question is that there is another variable to be picked up in the hourly report that gives a "negative demand" (I know) related to the reduction caused by the TES.

[cid:image007.png at 01D672CC.424DFB30]

Looking at your file, I am also not certain that the equipment control defined is actually linked to the chilled water loop.
[cid:image008.png at 01D672CC.424DFB30]

Hoping this helps - and very interesting study!

Cheers,

Brian


Footprint

Brian Fountain
Associate
d 416 572 8501 m 416 562 6831

From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Daric Adair via Equest-users
Sent: August 13, 2020 6:54 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] eQuest/DOE CHW Thermal Storage kW shift

CAUTION: EXTERNAL SENDER

Am working on a rather simple Chilled Water (CHW) Thermal Energy Storage (TES) System, but have run into an error where it does not appear that the kW is being shifted properly. Building in Las Vegas. Single Air-cooled Chiller using Chilled Water Storage to off-set demand charges. Testing the model with and without the TES, shows that the kW and costs are reduced, though maybe not as much as anticipated.

Digging into the model, the hourly reported kW from EM1-Cooling end-use and the Chiller kW consumption do not align. There is a single chiller; only cooling equipment in the model. Comparing the two with a HeatMap in the attached excel file shows that the EM1 does not drop off at all when the TES begins to discharge - but that the Chiller demand kW does. The Chiller kW is as expected; EM1 is not. In fact, EM1 with TES is only slightly less than EM1 without TES. Billing appears to be pegged to the EM1, thus, the cost reduction is not as much as expected. What is odd is that the annual sum of kW's and the daily SUMsubtotals between the EM1 and Chiller kW do align - what?! It is as if EM1 is not representing the kW shift that the Chiller is showing.

The CHW system does appear to charge, discharge, and track to the building load; so that is performing as expected.

The Utility rates are the same input and appear to be same on the output size. Equipment Controls and Load Management are different, b/c the non-TES doesnt have TES to charge/discharge.

So - why is the hourly kW from EM1-Cooling end-use different than the reported hourly kW from the chiller? Have scoured the DOE2 reference books and the Detail Report guide to no avail.

Thanks,
DARIC ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst

HENDERSON ENGINEERS<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hendersonengineers.com%2F%3Futm_source%3Dhei%26%26utm_medium%3Demail%26%26utm_campaign%3Dhei-shortsignature&data=02%7C01%7CNicholas.Caton%40se.com%7C7298b25b72204a99255608d8405e56d2%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637330121212958137&sdata=geWZR8l2fMdMVTWphaDOajyNo4%2FVg7VvK4Z4QEFo9ec%3D&reserved=0>
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>

LICENSED IN KS

HENDERSON PROUD SINCE 1970<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.hendersonengineers.com%2Fabout-us%2Four-story%2F%3Futm_source%3Dhei%26utm_medium%3Demail%26utm_campaign%3Dhei-shortsignature&data=02%7C01%7CNicholas.Caton%40se.com%7C7298b25b72204a99255608d8405e56d2%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C637330121212968127&sdata=z2KyH5ZKlDiRXfzAjjzykOLcc6RRgObaRrrhA9tr67Y%3D&reserved=0> | JUST GETTING STARTED.


________________________________

This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com<mailto:administrator at hendersonengineers.com>.

______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200817/c35188e3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 128763 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200817/c35188e3/attachment-0012.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 8477 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200817/c35188e3/attachment-0013.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 39442 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200817/c35188e3/attachment-0014.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 34724 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200817/c35188e3/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 126354 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200817/c35188e3/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 61952 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200817/c35188e3/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.jpg
Type: image/jpeg
Size: 1793 bytes
Desc: image009.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20200817/c35188e3/attachment-0002.jpg>


More information about the Equest-users mailing list