[Equest-users] Purchased Chilled Water Pumps
Jeff Ross-Bain
jeff at rbgb.com
Wed Sep 11 12:11:53 PDT 2019
Hi Bill,
And thanks for the quick response.
LEED V4 has added new requirements that reflect ASHRAE 90.1-2010. Previously LEED had Path 1 and Path 2 (per the document you referenced). Now, there is Path 1, 2, and 3, where Path 2, and 3, are the same as before, and Path 1 now refers to ASHRAE 90.1-2010 Appendix G and only applies to buildings where there is both purchased cooling and heating.
What I failed to mention is that we have both district cooling AND heating on this project.
So to reframe the question, per 90.1-2010, Appendix G, with purchased chilled water and heat, should the Baseline include a CHW pump even though the Proposed design does not have CHW pumps. 90.1-2010 language was a bit vague to me regarding that point.
Regards,
Jeff Ross-Bain, BCxP, BEMP, LEED Fellow, MSc
President
Charleston: 843-779-9229
Atlanta: 404-220-8955
RBGB<http://www.rbgb.com/>
Maximizing Building Performance.
From: Bishop, Bill <bbishop at pathfinder-ea.com>
Sent: Wednesday, September 11, 2019 1:41 PM
To: Jeff Ross-Bain <jeff at rbgb.com>
Cc: equest-users at lists.onebuilding.org
Subject: RE: Purchased Chilled Water Pumps
Hi Jeff,
The USGBC provided a guidance document for district thermal energy systems that should be helpful to you. The latest version is now 9 years old, but if you are modeling to 2010 Appendix G, it should be useable.
https://www.usgbc.org/resources/des-district-energy-systems-guidance-v22-and-v2009-guidance-v20
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image004.png at 01D568AF.1221FB00] Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Jeff Ross-Bain via Equest-users
Sent: Wednesday, September 11, 2019 1:23 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Purchased Chilled Water Pumps
Hi All,
I seem to get hung up on the basics.
Our project has purchased chilled water from a campus energy plant. The Proposed design does not have CHW pumps as the system is pressurized.
>From 90.1-2010, I am not sure if the Baseline model should include CHW pumps, or if they are omitted as in the Proposed.
Any thoughts would be helpful.
Many thanks!
Jeff Ross-Bain, BCxP, BEMP, LEED Fellow, MSc
President
[RBGB_Logo_Hi-Res]<http://www.rbgb.com/>
Charleston: 843-779-9229
Atlanta: 404-220-8955
www.rbgb.com<http://www.rbgb.com/>
Maximizing Building Performance
Join us at GREENBUILD 2019<https://www.greenbuildexpo.com/en/register.html> where two RBGB projects will be showcased.
[http://images.marketing.informaexhibitions.com/EloquaImages/clients/InformaGlobalExhibitionsIGE/%7bfb00d549-a115-4030-915b-c8c8d28094c2%7d_CRE19GRB-MM-RevisedEmailBanner.png]<https://www.greenbuildexpo.com/en/register.html>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190911/d8059f4b/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190911/d8059f4b/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1554 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190911/d8059f4b/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 3065 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190911/d8059f4b/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1884 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190911/d8059f4b/attachment-0002.jpg>
More information about the Equest-users
mailing list