[Equest-users] Electricity consumption mismatch between model and bill
Sharad Kumar
sharadcapricious at gmail.com
Sat Oct 26 20:50:53 PDT 2019
Hi Inga,
As per my understanding the correction that i can suggest is the correction
in schedules.
The electrical consumption that you are inferring in the eQUEST as 330 MWh
and the actual bills are 73 MWh.
Now you are as a suggestion is required to fetch the actual working hour of
the type wise hourly use of the segments.
There can be minor or major mismatch in the hourly usage which sometime can
have slight or above mismatch.
Kindly get the hourly usage data from the electrical consultant and if seen
do the correction in the schedules.
This is the only correction that i am able to think right now.
Hope this might help.
*Thank sand Regards,*
Sharad.Kumar
Freelancer
India..
-----------------------------------------------------------------------------------------------------------------------------
1. Electricity consumption mismatch between model and bill
(Inga Goebel)
---------- Forwarded message ----------
From: Inga Goebel <igoebel at duluthmn.gov>
To: "'equest-users at lists.onebuilding.org'" <
equest-users at lists.onebuilding.org>
Cc:
Bcc:
Date: Fri, 25 Oct 2019 19:52:53 +0000
Subject: [Equest-users] Electricity consumption mismatch between model and
bill
Hello,
I am currently struggling with a problem concerning the electricity
consumption of the building I modeled in eQuest. eQuest predicts a way
higher electricity consumption than it actually was billed for by the power
provider. eQuest predicts a usage of about 330 MWh a year and the actual
bills were at 73MWh for a year. Being sure that the power provider doesn’t
give away free electricity, I am currently trying to figure out where I
made a mistake.
One possible problem could be, that I included all the mechanicals (like
pumps, AHU, fan, unit heater, boiler,…) in the plug loads (misc.
equipment), which I read later, I should not do. But I am also not able to
find where I can correct it without going back to the wizard and losing all
my changes made in detailed mode. Now it is only shown as equipment load
which (if I understand correctly) includes my plug loads and also the
electricity consumption calculated by eQuest of the HVAC system. So is the
consumption of the HVAC system accounted for twice? Since I only want to
redo my plug loads, how can I do that without interfering with the eQuest
calculation of the HVAC electricity usage? Any help with that?
Also, these loads should not be a majority of the building and the overall
consumption will still be too high (at least that’s my guess). Anyone ever
had the same problem?
Lights consumption is about correct.
Thank you for your help.
Inga Goebel
_______________________________________________
Equest-users mailing list
Equest-users at lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20191027/bca57f8e/attachment.htm>
More information about the Equest-users
mailing list