[Equest-users] Delete plenum from existing model
Bishop, Bill
bbishop at pathfinder-ea.com
Fri Nov 22 06:16:11 PST 2019
Hi Shashank,
You can make the INT-WALL-TYPE of the ceiling surfaces ADIABATIC (no heat transfer across the surface) which eliminates the requirement for the NEXT-TO keyword.
A second option that may be easier is to copy your model and make the change in the Wizard mode. Once you take the revised model into DD Edit mode, you can open the input files of each model and copy the entire spaces section of the revised model into the other model. There’s more work to it though if you have already made many changes to loads in the spaces, as those changes are lost when you revert to Wizard mode and you’ll have to reenter them or copy them from the earlier model.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image005.png at 01D5A112.49557C00] Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Shashank Mishra via Equest-users
Sent: Friday, November 22, 2019 2:11 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Delete plenum from existing model
Hi Users
I am facing a challenge in deleting the plenum from each floor of the building. Initially, I have created a building with Flr to Ceil height of 9ft and Ceil to Flr height 4ft. Know I have to delete the plenum from each floor, in this process I have increased the Flr to Ceil height to 13ft, then tried to delete the plenum walls for each zone. After that, I am trying to delete the plenum space but the "Next to the surface" of the ceiling is which is selected as plenum are creating an error.
Please let me know the way to delete the plenum in detailed mode.
Thank you
Regards
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20191122/323ce07d/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20191122/323ce07d/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 1554 bytes
Desc: image005.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20191122/323ce07d/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1903 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20191122/323ce07d/attachment-0001.jpg>
More information about the Equest-users
mailing list