[Equest-users] Setting DOAS system type airflow rates
Chris Hadlock
cjhadlock at gmail.com
Thu May 16 11:17:04 PDT 2019
Hi Nick,
It was with the custom hourly outputs specific for DOAS systems that I
noticed this behaviour. I have no dehumidification controls specified (and
no dehumidification reheat energy indicated from my hourly reports). My
DOAS fan is set to run 24/7. The hourly reports show a heating load (and
corresponding fuel consumption) all hours of the year, even during cooling
hours. Using the hourly outputs available, I am unable to find out the
source of this heating load...really not sure what to make of it.
Chris
On Thu, May 16, 2019 at 1:04 PM Nicholas Caton <Nicholas.Caton at se.com>
wrote:
> Ah sorry, I retract my guess – I read too fast and my eyes locked to
> Brian’s demonstrative screenshot, which had a hot water loop indicated for
> heating.
>
>
>
> Taking a step back, have you tried some of the custom hourly outputs
> specific for DOAS systems? It may be helpful to figure out if this gas is
> being consumed 24/7, in sync with system operations, day vs. night, etc.
>
>
>
> One new thought is that this might be a piece of subcooling and reheat to
> accomplish dehumidification – something to look out for in those hourlies.
>
>
>
> ~Nick
>
>
>
> *Nick Caton, P.E., BEMP*
>
> Senior Energy Engineer
> Regional Energy Engineering Manager
>
> Energy and Sustainability Services
> Energy Performance Contracting
>
> D
> M
> F
> E
>
> 913 . 564 . 6361
>
> 785 . 410 . 3317
>
> 913 . 564 . 6380
>
> *nicholas.caton at se.com <nicholas.caton at se.com>*
>
> 15200 Santa Fe Trail Drive
> Suite 204
> Lenexa, KS 66219
> United States
>
>
>
>
>
> *From:* Equest-users <equest-users-bounces at lists.onebuilding.org> *On
> Behalf Of *Nicholas Caton via Equest-users
> *Sent:* Thursday, May 16, 2019 11:00 AM
> *To:* Chris Hadlock <cjhadlock at gmail.com>; Brian Fountain <
> Brian.Fountain at sa-footprint.com>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Setting DOAS system type airflow rates
>
>
>
> A fast shotgun guess: Is it possible the boiler(s) serving that hot water
> loop feature a 5:1 turndown and the loop operation is set to standby,
> meaning the boiler(s) can’t turn off completely?
>
>
>
> ~Nick
>
>
>
> *Nick Caton, P.E., BEMP*
>
> Senior Energy Engineer
> Regional Energy Engineering Manager
>
> Energy and Sustainability Services
> Energy Performance Contracting
>
> D
> M
> F
> E
>
> 913 . 564 . 6361
>
> 785 . 410 . 3317
>
> 913 . 564 . 6380
>
> *nicholas.caton at se.com <nicholas.caton at se.com>*
>
> 15200 Santa Fe Trail Drive
> Suite 204
> Lenexa, KS 66219
> United States
>
>
>
>
>
> *From:* Equest-users <equest-users-bounces at lists.onebuilding.org> *On
> Behalf Of *Chris Hadlock via Equest-users
> *Sent:* Thursday, May 16, 2019 9:16 AM
> *To:* Brian Fountain <Brian.Fountain at sa-footprint.com>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Setting DOAS system type airflow rates
>
>
>
> For my most recent project for which I have a DOAS system, I've noticed a
> constant (8760 hrs) heating energy consumption. I've got the DOAS set up as
> a gas-fired furnace and DX cooling coil. I've set my auxiliary fuel
> consumption set to 0 and no preheat. During the summer where there is
> active cooling my furnace is running at about 19% of it's design capacity
> (simultaneous heating and cooling). Has anyone noticed their DOAS system
> doing this? Any suggestions?
>
>
>
> Thanks,
>
> Chris
>
>
>
> On Wed, May 15, 2019 at 9:52 AM Brian Fountain via Equest-users <
> equest-users at lists.onebuilding.org> wrote:
>
> Hi Chris.
>
>
>
> Yes – you can explicitly set the heating and/or cooling capacities of the
> DOAS system type.
>
>
>
>
>
> Cheers,
>
>
>
> Brian
>
>
>
>
>
> *Footprint *
> *Brian Fountain *Associate
> d 416 572 8501 m 416 562 6831
>
>
>
> *From:* Equest-users <equest-users-bounces at lists.onebuilding.org> *On
> Behalf Of *Jones, Christopher via Equest-users
> *Sent:* Wednesday, May 15, 2019 8:39 AM
> *To:* Bishop, Bill <bbishop at pathfinder-ea.com>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Setting DOAS system type airflow rates
>
>
>
> CAUTION: EXTERNAL SENDER
>
> Thanks Bill,
>
> Re. DOAS coils – is there an option to specifically size the coils?
>
>
>
> *Christopher R Jones, P.Eng.*
>
> T+ 1 416-644-0252
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *Bishop, Bill
> via Equest-users
> *Sent:* Tuesday, May 14, 2019 2:02 PM
> *To:* Brian Fountain <Brian.Fountain at sa-footprint.com>
> *Cc:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] Setting DOAS system type airflow rates
>
>
>
> Thanks, Brian! You make an important point on design sizing of DOAS
> systems – the hourly ventilation rate is determined by the systems/zones
> that the DOAS serves, and the corresponding ventilation controls for those
> systems.
>
> Some additional observations:
>
> - If you enter the DOAS SUPPLY-FLOW (Design cfm):
>
> o The design fan power will be based on the SUPPLY-FLOW multiplied by
> SUPPLY-KW/FLOW (if entered).
>
> o Any central airhandler coils will be autosized based on the
> SUPPLY-FLOW. (See the SV-C report in the SIM file.)
>
> - If instead, you let the DOAS SUPPLY-FLOW (Design cfm) default
> by leaving it blank:
>
> o The design fan power will be based on the design ventilation rate
> determined by the served systems multiplied by SUPPLY-KW/FLOW (if entered).
>
> o Any central airhandler coils will be autosized based on the design
> ventilation rate.
>
> - If you enter zone ventilation as OA/FLOW-PER (cfm per person),
> to simulate DCV or to size the ventilation per ASHRAE 62.1 guidelines, the
> design ventilation rate will be based on the highest hourly value in the
> occupancy schedule. So you have to have at least one hour with 1.0
> occupancy either in the weekday, weekend and/or CDD/HDD schedules.
> Otherwise, the design ventilation rate will be reduced.
>
>
>
> ~Bill
>
>
>
> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP*
>
> *Senior Energy Engineer*
>
>
>
> [image: Pathfinder-EA-logo-2]*T: (585) 698-1956 * F:
> (585) 325-6005
>
> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
> www.pathfinder-ea.com
> <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.pathfinder-ea.com%2F&data=02%7C01%7CNicholas.Caton%40se.com%7Cf8a85f5edc2c42cdb59508d6da17969f%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936192180474764&sdata=ZxSS6IfOqstH6v3zU5dyJpYkPxBde709aBQo0vu81KU%3D&reserved=0>
>
> 134 South Fitzhugh Street
>
> Rochester, NY 14608 *Ask me why Carbon Fee &
> Dividend may be right for you.*
>
>
>
> *From:* Equest-users <equest-users-bounces at lists.onebuilding.org> *On
> Behalf Of *Brian Fountain via Equest-users
> *Sent:* Monday, May 13, 2019 5:47 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* [Equest-users] Setting DOAS system type airflow rates
>
>
>
> Caution note when using DOAS systems – you cannot simply define the OA
> volume in the flow parameters tab of the DOAS fan.
>
>
>
> In DOE-2.3, there is now a system type ‘DOAS’ that will properly provide
> outdoor air either directly to zones or to the mixing section of the system
> it serves. The volume of outdoor air delivered by this system is
> determined by the outdoor air flow rates of the zones that take air from
> this system. The screenshot below suggests that the unit will be
> delivering 6,545 cfm of OA but in fact this system was only delivering 500
> cfm as the served zones did not have their OA volumes set properly.
>
>
>
>
>
> When the OA was defined in the zones taking air from this system, the
> volume of OA in the DOAS was as expected.
>
>
>
> Today’s lesson – define outdoor air rates properly, and hourly reports are
> your friend.
>
>
>
>
>
>
>
> *Footprint **Brian Fountain *P.Eng., LEED AP BD+C, BEMP
> Associate
> Brian.Fountain at sa-footprint.com
>
> 100 Sheppard Ave Suite 800 Toronto Ontario M2N 6Z1
> t 416 218 7025 f 416 487 9104 sa-footprint.com
> <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fsa-footprint.com&data=02%7C01%7CNicholas.Caton%40se.com%7Cf8a85f5edc2c42cdb59508d6da17969f%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936192180484759&sdata=FLelrlwoR460pnUjFRSbzxhggmHBj0%2BuuF5nqEX4cnY%3D&reserved=0>
>
> Vancouver Calgary Edmonton Winnipeg Kitchener Toronto Ottawa
>
>
>
>
> ------------------------------
>
>
>
> NOTICE: This communication and any attachments ("this message") may
> contain information which is privileged, confidential, proprietary or
> otherwise subject to restricted disclosure under applicable law. This
> message is for the sole use of the intended recipient(s). Any unauthorized
> use, disclosure, viewing, copying, alteration, dissemination or
> distribution of, or reliance on, this message is strictly prohibited. If
> you have received this message in error, or you are not an authorized or
> intended recipient, please notify the sender immediately by replying to
> this message, delete this message and all copies from your e-mail system
> and destroy any printed copies. You are receiving this communication
> because you are listed as a current WSP contact. Should you have any
> questions regarding WSP's electronic communications policy, please consult
> our Anti-Spam Commitment at www.wsp.com/casl
> <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.wsp.com%2Fcasl&data=02%7C01%7CNicholas.Caton%40se.com%7Cf8a85f5edc2c42cdb59508d6da17969f%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936192180494753&sdata=FRdufR7Z8P4uFzL3ZBr7w1DJ%2FfjFDiw07iVMbqZJr10%3D&reserved=0>.
> For any concern or if you believe you should not be receiving this message,
> please forward this message to caslcompliance at wsp.com so that we can
> promptly address your request. Note that not all messages sent by WSP
> qualify as commercial electronic messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »),
> peut contenir des renseignements ou de l'information privilégiés,
> confidentiels, propriétaires ou à divulgation restreinte en vertu de la
> loi. Ce message est destiné à l'usage exclusif du/des destinataire(s)
> voulu(s). Toute utilisation non permise, divulgation, lecture,
> reproduction, modification, diffusion ou distribution est interdite. Si
> vous avez reçu ce message par erreur, ou que vous n'êtes pas un
> destinataire autorisé ou voulu, veuillez en aviser l'expéditeur
> immédiatement et détruire le message et toute copie électronique ou
> imprimée. Vous recevez cette communication car vous faites partie des
> contacts de WSP. Si vous avez des questions concernant la politique de
> communications électroniques de WSP, veuillez consulter notre Engagement
> anti-pourriel au www.wsp.com/lcap
> <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.wsp.com%2Flcap&data=02%7C01%7CNicholas.Caton%40se.com%7Cf8a85f5edc2c42cdb59508d6da17969f%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936192180494753&sdata=rsHWpRnirnqYRmdoN3vvQLmiiAu4XqWruM09935fFRI%3D&reserved=0>.
> Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce
> message, prière de le transférer au conformitelcap at wsp.com afin que nous
> puissions rapidement traiter votre demande. Notez que ce ne sont pas tous
> les messages transmis par WSP qui constituent des messages electroniques
> commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7CNicholas.Caton%40se.com%7Cf8a85f5edc2c42cdb59508d6da17969f%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936192180494753&sdata=hx6AyJtaKdTQPYGptZDAFMkyOzZXksf4%2FKllt9%2BxGdQ%3D&reserved=0>
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
>
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/d54bab9e/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/d54bab9e/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/d54bab9e/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 32288 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/d54bab9e/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1860 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/d54bab9e/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1900 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/d54bab9e/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1554 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/d54bab9e/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 31943 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/d54bab9e/attachment-0002.jpg>
More information about the Equest-users
mailing list