[Equest-users] Setting DOAS system type airflow rates
Brian Fountain
Brian.Fountain at sa-footprint.com
Mon May 13 14:46:56 PDT 2019
Caution note when using DOAS systems - you cannot simply define the OA volume in the flow parameters tab of the DOAS fan.
In DOE-2.3, there is now a system type 'DOAS' that will properly provide outdoor air either directly to zones or to the mixing section of the system it serves. The volume of outdoor air delivered by this system is determined by the outdoor air flow rates of the zones that take air from this system. The screenshot below suggests that the unit will be delivering 6,545 cfm of OA but in fact this system was only delivering 500 cfm as the served zones did not have their OA volumes set properly.
[cid:image003.jpg at 01D509B3.D8F50570]
When the OA was defined in the zones taking air from this system, the volume of OA in the DOAS was as expected.
Today's lesson - define outdoor air rates properly, and hourly reports are your friend.
Footprint
Brian Fountain P.Eng., LEED AP BD+C, BEMP
Associate
Brian.Fountain at sa-footprint.com
100 Sheppard Ave Suite 800 Toronto Ontario M2N 6Z1
t 416 218 7025 f 416 487 9104 sa-footprint.com
Vancouver Calgary Edmonton Winnipeg Kitchener Toronto Ottawa
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190513/6088ebb4/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 31943 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190513/6088ebb4/attachment.jpg>
More information about the Equest-users
mailing list