[Equest-users] Setting DOAS system type airflow rates
doug at maddoxenergy.com
doug at maddoxenergy.com
Thu May 16 12:04:51 PDT 2019
Your COOL-SET-T and MIN-SUPPLY-T are both defaulting to 65 F, which results in cooling and reheating. The solution is to drop your heating setpoint slightly and enter cooling setpoints that are slightly higher than the heating setpoint, as in the attached file.
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Chris Hadlock via Equest-users
Sent: Thursday, May 16, 2019 2:33 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Setting DOAS system type airflow rates
It's been suggested I share my pd2 and inp (and weather) file to allow others to perhaps help with the troubleshooting. Those 3 files have been attached. I am using build 7175, DOE 2.3.
Thank you to all that take a look and provide suggestions.
Chris
On Thu, May 16, 2019 at 12:00 PM Nicholas Caton <Nicholas.Caton at se.com <mailto:Nicholas.Caton at se.com> > wrote:
A fast shotgun guess: Is it possible the boiler(s) serving that hot water loop feature a 5:1 turndown and the loop operation is set to standby, meaning the boiler(s) can’t turn off completely?
~Nick
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Energy Performance Contracting
D
M
F
E
913 . 564 . 6361
785 . 410 . 3317
913 . 564 . 6380
<mailto:nicholas.caton at se.com> nicholas.caton at se.com
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
From: Equest-users <equest-users-bounces at lists.onebuilding.org <mailto:equest-users-bounces at lists.onebuilding.org> > On Behalf Of Chris Hadlock via Equest-users
Sent: Thursday, May 16, 2019 9:16 AM
To: Brian Fountain <Brian.Fountain at sa-footprint.com <mailto:Brian.Fountain at sa-footprint.com> >
Cc: equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Setting DOAS system type airflow rates
[External email: Use caution with links and attachments]
_____
For my most recent project for which I have a DOAS system, I've noticed a constant (8760 hrs) heating energy consumption. I've got the DOAS set up as a gas-fired furnace and DX cooling coil. I've set my auxiliary fuel consumption set to 0 and no preheat. During the summer where there is active cooling my furnace is running at about 19% of it's design capacity (simultaneous heating and cooling). Has anyone noticed their DOAS system doing this? Any suggestions?
Thanks,
Chris
On Wed, May 15, 2019 at 9:52 AM Brian Fountain via Equest-users <equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org> > wrote:
Hi Chris.
Yes – you can explicitly set the heating and/or cooling capacities of the DOAS system type.
Cheers,
Brian
Footprint
Brian Fountain
Associate
d 416 572 8501 m 416 562 6831
From: Equest-users <equest-users-bounces at lists.onebuilding.org <mailto:equest-users-bounces at lists.onebuilding.org> > On Behalf Of Jones, Christopher via Equest-users
Sent: Wednesday, May 15, 2019 8:39 AM
To: Bishop, Bill <bbishop at pathfinder-ea.com <mailto:bbishop at pathfinder-ea.com> >
Cc: equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Setting DOAS system type airflow rates
CAUTION: EXTERNAL SENDER
Thanks Bill,
Re. DOAS coils – is there an option to specifically size the coils?
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill via Equest-users
Sent: Tuesday, May 14, 2019 2:02 PM
To: Brian Fountain <Brian.Fountain at sa-footprint.com <mailto:Brian.Fountain at sa-footprint.com> >
Cc: equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Setting DOAS system type airflow rates
Thanks, Brian! You make an important point on design sizing of DOAS systems – the hourly ventilation rate is determined by the systems/zones that the DOAS serves, and the corresponding ventilation controls for those systems.
Some additional observations:
- If you enter the DOAS SUPPLY-FLOW (Design cfm):
o The design fan power will be based on the SUPPLY-FLOW multiplied by SUPPLY-KW/FLOW (if entered).
o Any central airhandler coils will be autosized based on the SUPPLY-FLOW. (See the SV-C report in the SIM file.)
- If instead, you let the DOAS SUPPLY-FLOW (Design cfm) default by leaving it blank:
o The design fan power will be based on the design ventilation rate determined by the served systems multiplied by SUPPLY-KW/FLOW (if entered).
o Any central airhandler coils will be autosized based on the design ventilation rate.
- If you enter zone ventilation as OA/FLOW-PER (cfm per person), to simulate DCV or to size the ventilation per ASHRAE 62.1 guidelines, the design ventilation rate will be based on the highest hourly value in the occupancy schedule. So you have to have at least one hour with 1.0 occupancy either in the weekday, weekend and/or CDD/HDD schedules. Otherwise, the design ventilation rate will be reduced.
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
T: (585) 698-1956 F: (585) 325-6005
<mailto:wbishop at pathfinder-ea.com> bbishop at pathfinder-ea.com <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.pathfinder-ea.com%2F&data=02%7C01%7CNicholas.Caton%40se.com%7C8779c580c4e341769e4a08d6da090db2%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936129752252494&sdata=cW5ywD3jl4zameXVIYXruYvWkV2%2FQG7Zgc%2BgtLYhOvM%3D&reserved=0> www.pathfinder-ea.com
134 South Fitzhugh Street
Rochester, NY 14608 Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org <mailto:equest-users-bounces at lists.onebuilding.org> > On Behalf Of Brian Fountain via Equest-users
Sent: Monday, May 13, 2019 5:47 PM
To: equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Setting DOAS system type airflow rates
Caution note when using DOAS systems – you cannot simply define the OA volume in the flow parameters tab of the DOAS fan.
In DOE-2.3, there is now a system type ‘DOAS’ that will properly provide outdoor air either directly to zones or to the mixing section of the system it serves. The volume of outdoor air delivered by this system is determined by the outdoor air flow rates of the zones that take air from this system. The screenshot below suggests that the unit will be delivering 6,545 cfm of OA but in fact this system was only delivering 500 cfm as the served zones did not have their OA volumes set properly.
When the OA was defined in the zones taking air from this system, the volume of OA in the DOAS was as expected.
Today’s lesson – define outdoor air rates properly, and hourly reports are your friend.
Footprint
Brian Fountain P.Eng., LEED AP BD+C, BEMP
Associate
Brian.Fountain at sa-footprint.com <mailto:Brian.Fountain at sa-footprint.com>
100 Sheppard Ave Suite 800 Toronto Ontario M2N 6Z1
t 416 218 7025 f 416 487 9104 sa-footprint.com <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fsa-footprint.com&data=02%7C01%7CNicholas.Caton%40se.com%7C8779c580c4e341769e4a08d6da090db2%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936129752257477&sdata=twEy2v5cdWidn0AE4jAzjGgdQn1RJsTwy9JAvs%2BSHWo%3D&reserved=0>
Vancouver Calgary Edmonton Winnipeg Kitchener Toronto Ottawa
_____
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.wsp.com%2Fcasl&data=02%7C01%7CNicholas.Caton%40se.com%7C8779c580c4e341769e4a08d6da090db2%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936129752262471&sdata=VKkoGXV71zjkgLiTaLRAzn8VawCw%2FV%2B6A6cvUhOyrmA%3D&reserved=0> . For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com <mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.wsp.com%2Flcap&data=02%7C01%7CNicholas.Caton%40se.com%7C8779c580c4e341769e4a08d6da090db2%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936129752267461&sdata=hKGz1sDU5yoH92pgs2tEjkl85TyN4I532i8zghQf73I%3D&reserved=0> . Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com <mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org <https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7CNicholas.Caton%40se.com%7C8779c580c4e341769e4a08d6da090db2%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636936129752272458&sdata=5AJjzvPVXhL3Pf3kyi76i01U9UUWvcM9tgep5R75rpU%3D&reserved=0>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/146c840c/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/146c840c/attachment-0012.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/146c840c/attachment-0013.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 32288 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/146c840c/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1860 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/146c840c/attachment-0014.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1900 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/146c840c/attachment-0010.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1554 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/146c840c/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 31943 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/146c840c/attachment-0011.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Res_Mod.inp
Type: application/octet-stream
Size: 283766 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190516/146c840c/attachment-0003.obj>
More information about the Equest-users
mailing list