[Equest-users] reducing unmet hours with thermostat settings/controls
Jones, Christopher
Christopher.r.Jones at wsp.com
Thu Mar 28 10:42:55 PDT 2019
Bill,
I typically adjust the heating min air low to reduce unmet hours. I have never had an issue under review.
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image001.png at 01D4E56C.24678620]
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Thursday, March 28, 2019 11:39 AM
To: Jones, Christopher <Christopher.r.Jones at wsp.com>
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] reducing unmet hours with thermostat settings/controls
All,
Does anyone have a different suggestion on addressing unmet hours in VAV systems that best meets the intent of 90.1 simulation?
As Christopher points out, the PNNL 90.1-2010 PRM Reference Manual (linked below ) requires “single maximum” thermostat control for VAV zones (PROPORTIONAL in DOE-2/eQUEST). The heating airflow is not permitted to increase above 30% minimum flow (ZONE:MIN-FLOW-RATIO = 0.3). I have never interpreted G3.1.3.13 this way and have been using REVERSE-ACTION thermostats with ZONE:HMAX-FLOW-RATIO = 1.0 to address unmet heating hours in both Baseline and Proposed models. (HMAX-FLOW-RATIO = 0.5 or 0.6 is often sufficient.) This is easy to implement through zone defaults and minimizes adjustments to individual zones. If you have to use PROPORTIONAL thermostat control, I think you would need to increase the ZONE:HMIN-FLOW-RATIO above 0.3 or increase the SYSTEM:SIZING-RATIO.
Thanks,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image006.png at 01D4E56C.245B5120] Ask me why Carbon Fee & Dividend may be right for you.
From: Jones, Christopher <Christopher.r.Jones at wsp.com<mailto:Christopher.r.Jones at wsp.com>>
Sent: Thursday, March 28, 2019 7:01 AM
To: Bishop, Bill <bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] reducing unmet hours with thermostat settings/controls
Hi Bill,
The PNNL document is, ASHRAE Standard 90.1-2010 Performance Rating Method Reference Manual, May 2016. The manual addresses 90.1-2010 Appendix G.
Dual maximum control is achieved using THERMOSTAT-TYPE = REVERSE-ACTION. The baseline model would use Single Maximum (PROPORTIONAL). See page 124 in the document.
https://www.pnnl.gov/main/publications/external/technical_reports/PNNL-25130.pdf
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image007.png at 01D4E56C.245B5120]
From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Wednesday, March 27, 2019 9:54 AM
To: Jones, Christopher <Christopher.r.Jones at wsp.com<mailto:Christopher.r.Jones at wsp.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] reducing unmet hours with thermostat settings/controls
Christopher,
* Which PNNL manual are you referring to and can you provide a link?
* What modeling applications do you use it for (LEED, code compliance, other baselines etc.)?
* Is dual maximum control the same as TWO-POSITION in DOE-2/eQUEST?
* What THERMOSTAT-TYPE would you recommend for a baseline if different from a proposed design (and is there language anywhere that supports/allows it)?
Thanks,
~Bill
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Jones, Christopher via Equest-users
Sent: Tuesday, March 26, 2019 6:18 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Hourly space temperature after cooling
Spoke too soon. The PNNL manual promotes Dual Maximum control for VAV boxes. But it doesn’t apply to the baseline.
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image007.png at 01D4E56C.245B5120]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher via Equest-users
Sent: Tuesday, March 26, 2019 6:13 PM
To: Nicholas Caton <Nicholas.Caton at se.com<mailto:Nicholas.Caton at se.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Hourly space temperature after cooling
I agree with Nick’s points. I find adjusting the baseline model minimum heating flows takes time. I have many models where zones need a higher minimum flow than 0.4cfm/sf, 30% in 90.1-2010. I also question the use of REVERSE ACTION thermostats for the baseline VAV box control. I have only come across one building with reverse action VAV boxes.
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image007.png at 01D4E56C.245B5120]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton via Equest-users
Sent: Tuesday, March 26, 2019 12:46 PM
To: The Energy Simulation Academy <info at simulate.energy<mailto:info at simulate.energy>>; Integral Mechanical Engineering Designs <integralmech at outlook.com<mailto:integralmech at outlook.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Hourly space temperature after cooling
I have a training/teaching topic I’ve delivered around the subject of unmet hours… it includes this definition (my technical understanding):
An unmet hour is reported when a zone’s hourly temperature diverges from the thermostat setpoint/setback temperature by at least the throttling range + 1°F.
Further, because this definition in isolation (and the associated reference manual entries on the topic) can lead other astray without further context, I immediately follow this definition with the following:
A popular misconception is that throttling range is a panacea for resolving unmet hours.
Tweaking throttling range in isolation however is rarely an effective "treatment" for unmet hours in practice. It does not address any of the most common root causes/resolutions for unmet hours (to my experience):
· Inadequate capacities:
* airflow
* heating
* cooling
* Emphasis for inadequate airflow: Where a model relies heavily upon auto-sizing, airflow by far the most common capacity issue I’ve encountered when troubleshooting.
· System / conditioning availability (scheduling / night-cycling / lockouts)
· Assumptions / errors for the inputs concerning the interior & envelope loads being handled by the systems
· End-user vs. interface errors in developing/tweaking thermostat schedules within the eQuest interface.
· Thermostat schedules being automatically assigned from wizards and therefore reporting unmet hours where comfort isn’t truly being measured/maintained in real life (i.e. does anyone really care if a garage gets warm in the summer?).
This isn’t really a “computational” response in hindsight, but I had this material at-hand to easily share. Hope this helps in any case!
~Nick
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of The Energy Simulation Academy via Equest-users
Sent: Tuesday, March 26, 2019 10:38 AM
To: Integral Mechanical Engineering Designs <integralmech at outlook.com<mailto:integralmech at outlook.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Hourly space temperature after cooling
Good for you! But now my OCD is triggered.
To repeat the question if anyone is just looking at this email:
Does anyone happen to know the computational definition of an unmet hour for eQUEST? Especially as stated:
i.e DOE2 will mark an Unmet hour if a zone is: Outside the throttling range? How many degrees outside range (.1, 1 etc)? Plus Occupied? Plus Coil capacities are exceeded? Plus Any other conditions?
I guess I can dig for it, but it's likely one of you knows this officially,
Bob
Energy-models.com
Simulate.Energy
[Image removed by sender.]ᐧ
On Tue, Mar 26, 2019 at 10:28 AM Integral Mechanical Engineering Designs via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
Hello,
Thank you for all your answers. There have been really helpful, and the problem was that I had 90 °F in the day schedules within the S1 Sys1 (PSZ) Cool SCH (different value as mentioned by Bill). The solution was to correct the value to 75 °F, and now the unmet hours match with the SS-O report.
Kind Regards,
Paul Caicedo
Mechanical Engineering Consultant
IntegralMECH
________________________________
From: Bishop, Bill <bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>>
Sent: March 25, 2019 7:27 AM
To: Integral Mechanical Engineering Designs; David Eldridge
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: Hourly space temperature after cooling
Hi Paul,
The 75 °F input that you shared below for “Indoor Design Temperature” is the DESIGN-COOL-T which is used for sizing calculations (and is optional when using DOE-2.3). The hourly thermostat setpoint is part of the thermostat schedule so you need to look at the day schedules within the S1 Sys1 (PSZ) Cool Sch.
Regards,
~Bill
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Integral Mechanical Engineering Designs via Equest-users
Sent: Saturday, March 23, 2019 2:34 PM
To: David Eldridge <DEldridge at grummanbutkus.com<mailto:DEldridge at grummanbutkus.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Hourly space temperature after cooling
Hi David,
Thanks for the answer. I don´t think that explain the data because the system is working most of the time during the year, and a note in the SS-O report shows that the temperature counts are made only for the hours when the fans are on. The cooling schedule matches with the occupancy schedule.
[cid:image009.png at 01D4E56C.245B5120]
The set point is 75 °F and the throttle range is 2 °R.
[cid:image010.png at 01D4E56C.245B5120]
The BEPS report shows that are 155 unmet hours, but the SS-O report gives a value of at least 2505 (adding from 80-85 and above 85).
Kind Regards,
Paul Caicedo
Mechanical Engineering Consultant
IntegralMECH
From: David Eldridge <DEldridge at grummanbutkus.com<mailto:DEldridge at grummanbutkus.com>>
Sent: March 22, 2019 9:29 AM
To: Integral Mechanical Engineering Designs
Subject: RE: Hourly space temperatura after cooling
That SS-O report should be after cooling (it’s a “system” report), but it may include some hours when the control system is in setback – it’s not only for occupied hours, would that explain your data?
There is a separate module for report variables that you can specify to document any number of internal calculations, including one or more space temperatures – it’s been a while since I set one of those up but if you search this community for “report variables” some instructions should pop up.
These can then also be exported to excel, or printed in the *.sim report.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Associate
Direct: (847) 316-9224 | Mobile: (773) 490-5038
Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201
Energy Efficiency Consultants and Sustainable Design Engineers
grummanbutkus.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fgrummanbutkus.com%2F&data=02%7C01%7CNicholas.Caton%40se.com%7C554c32e1d9244322c3f208d6b201173d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892115095564054&sdata=yfOaDES%2BOzvQv3iKgNTZvZnm3EaV4AHHfLwYfHJi76Y%3D&reserved=0> | Blog<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fgrummanbutkus.com%2Fblog&data=02%7C01%7CNicholas.Caton%40se.com%7C554c32e1d9244322c3f208d6b201173d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892115095574062&sdata=P10jrl8jljIXGxoyhaLbS9n4PwNMm%2FvBlascS5hTzcQ%3D&reserved=0> | Facebook<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FGrummanButkus-Associates%2F1385285015032526&data=02%7C01%7CNicholas.Caton%40se.com%7C554c32e1d9244322c3f208d6b201173d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892115095584070&sdata=gWOrY0S7gQCM8sMy%2FV51rW%2FC7B9whhKN7X%2BEiGbWX10%3D&reserved=0> | Twitter<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fgrummanbutkus&data=02%7C01%7CNicholas.Caton%40se.com%7C554c32e1d9244322c3f208d6b201173d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892115095584070&sdata=iqLqxI1zpJOVJ%2BzyUlxDh1dmVHWn8Pa0%2B90oIGulfrM%3D&reserved=0>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Integral Mechanical Engineering Designs via Equest-users
Sent: Friday, March 22, 2019 8:51 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Hourly space temperatura after cooling
Hi all,
If I open the BEPS Building Energy Performance, there are 155 unmet hours. I would like to get the temperature values throughout the year after cooling, but the only related option that I can see is the SS-O Space Temperature Summary where the temperatures above the set point are much more than the unmet hours. It seems that is the report of the space before cooling.
How could I get the space temperature after cooling to have relation with the unmet hours?
Kind Regards,
Paul Caicedo
Mechanical Engineering Consultant
IntegralMECH
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7CNicholas.Caton%40se.com%7C554c32e1d9244322c3f208d6b201173d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892115095594079&sdata=JhV8ekCPibR8ipR%2BOd3K%2Fd%2Ffizgun7wHyJTcV4kARZU%3D&reserved=0>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
The Energy Simulation Academy
[https://docs.google.com/uc?export=download&id=1HlkgKdB26cSbEQN-U6d4hm8Zg-jrpCyg&revid=0B1vD4jOXrCvQVGdobk9laElydW5hYU0wUVphVUUyRlUyZFZZPQ]<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fsimulate.energy%2F&data=02%7C01%7CNicholas.Caton%40se.com%7C554c32e1d9244322c3f208d6b201173d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892115095604091&sdata=59bJv62EXyg47UaIcrgo8AvuILCzksRo3Dlxrs%2BWOPo%3D&reserved=0>
Simulate.Energy<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fsimulate.energy%2F&data=02%7C01%7CNicholas.Caton%40se.com%7C554c32e1d9244322c3f208d6b201173d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892115095604091&sdata=59bJv62EXyg47UaIcrgo8AvuILCzksRo3Dlxrs%2BWOPo%3D&reserved=0>
Follow us on Linkedin<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fin%2Fthe-energy-simulation-academy-tesa-42584b16b%2F&data=02%7C01%7CNicholas.Caton%40se.com%7C554c32e1d9244322c3f208d6b201173d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892115095614095&sdata=Oja3Bkf%2FqrHtZOh%2Fh0R4KybGSpU6PSyHQ1nXQAcJdUk%3D&reserved=0> and Facebook<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fgroups%2F245943612664667%2F%3Fref%3Dbookmarks&data=02%7C01%7CNicholas.Caton%40se.com%7C554c32e1d9244322c3f208d6b201173d%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636892115095614095&sdata=c13541SlnjjoU76741k1Tt%2FW4BeutqPXmYUhZ5UZRS4%3D&reserved=0>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1554 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 1860 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 823 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 14382 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 5238 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 144 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 1860 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment-0005.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1882 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190328/47d80e77/attachment-0002.jpg>
More information about the Equest-users
mailing list