[Equest-users] NECB 2015 Question
Menush Akbari
makbari at missiongreenbuildings.com
Thu Mar 14 16:30:03 PDT 2019
Hi Chris,
I agree as well, that’s how we’ve been interpreting it. Basically in Calgary climate zone 7A if the proposed design has a 20% FDWR then the reference building can be set to 33%. And there’s also an allowable skylight area (I think it’s 5% or less?) which can be applied to the reference building as well.
Cheers,
Menush Akbari BEng, PEng, BEMP, CMVP
Associate Principal, Energy
c 250 777 3380
[cid:image002.jpg at 01D4DA83.2B1BA530]
Calgary | Nelson
missiongreenbuildings.com<http://missiongreenbuildings.com/>
Member of Integral Group
From: Chris Hadlock <cjhadlock at gmail.com>
Sent: Thursday, March 14, 2019 8:10 AM
To: Benjamin Zizi <bzizi at ecohabitation.com>
Cc: Kyle Anders <kyle at buildingknowledge.ca>; Brian Fountain <bfountain at greensim.com>; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] NECB 2015 Question
Thanks you to all the respondents. I've had 3 consistent responses that in fact the Reference window area is to be set to the maximum allowable in all cases (for the NECB code), which I'll take as general (modeler's) agreement.
Cheers,
Chris
On Thu, Mar 14, 2019 at 10:47 AM Benjamin Zizi <bzizi at ecohabitation.com<mailto:bzizi at ecohabitation.com>> wrote:
Good morning,
That would be my interpretation too. It differs if it is more or less than the maximum permitted and should be adjusted for the reference as maximum permitted.This approach is different than with ASHRAE 90.1 and gives a significant advantage to projects with less windows than usual (which is a good thing). Same approach is taken with Energuide ratings : HOT2000 software adjust the ratio of reference building as soon as the proposed building is outside the minimum and maximum ranges : 17% - 22%.
This interpretation would also be confirmed by the LEED V4 Canadian ACP (https://www.cagbc.org/cagbcdocs/leed/LEED_v4_Canadian_ACP_Language_as_of_20170420.pdf<https://mandrillapp.com/track/click/30634852/www.cagbc.org?p=eyJzIjoiWW42Zi0wVWI5amt1SjNDblB3ODI3Uk12Wkc0IiwidiI6MSwicCI6IntcInVcIjozMDYzNDg1MixcInZcIjoxLFwidXJsXCI6XCJodHRwczpcXFwvXFxcL3d3dy5jYWdiYy5vcmdcXFwvY2FnYmNkb2NzXFxcL2xlZWRcXFwvTEVFRF92NF9DYW5hZGlhbl9BQ1BfTGFuZ3VhZ2VfYXNfb2ZfMjAxNzA0MjAucGRmXCIsXCJpZFwiOlwiNWY3OTIxYzMxNmYxNGMyY2IwZDRlOThmZTZkM2JhODdcIixcInVybF9pZHNcIjpbXCJlNDE5ZDNiNzViMjM2NjhhYTM0ZmMzYjYwZDViMzZhNWIxNzJhZTIxXCJdfSJ9>) that states that projects can use the NECB reference at some conditions, including :
Apply fenestration area convention similar to ASHRAE 90.1-2010
Maintain the same FWR (as defined by NECB, including doors) for the Reference as exists in the Proposed Design, up to the prescribed maximum. If the Proposed Design’s FWR exceeds the prescribed FWR, scale down the fenestrations in the Reference case accordingly.
However, NECB is quite unclear on this topic and it could be good to have an official guidance :)
[https://docs.google.com/uc?export=download&id=1J_zvh5BNZU3Pav6uMIXQtaMtvMKiVkmY&revid=0B6eGch-syESxNHlWbWdFdVpDQmp0aGU5SlkybEpEcFlBSHNJPQ]
Benjamin Zizi
Coordonnateur technique
Évaluateur écologique et énergétique LEED Habitations
Évaluations Écohabitation
6001, rue St-Hubert | Montréal QC | H2S 2L8
514.985.0004 poste 613 | 1 855.400.0326
ecohabitation.com<https://mandrillapp.com/track/click/30634852/ecohabitation.com?p=eyJzIjoiSmRTVWIwaDZIRmVHWHNDUmlkTkJxZzBQTHRvIiwidiI6MSwicCI6IntcInVcIjozMDYzNDg1MixcInZcIjoxLFwidXJsXCI6XCJodHRwOlxcXC9cXFwvZWNvaGFiaXRhdGlvbi5jb21cXFwvXCIsXCJpZFwiOlwiNWY3OTIxYzMxNmYxNGMyY2IwZDRlOThmZTZkM2JhODdcIixcInVybF9pZHNcIjpbXCJkOTdkNTIzZjJkZmI4ZTcyYmI5Yzg5NTkwZTNlZTc5YjBmNTNjMWM0XCJdfSJ9>
Suivez-nous !
facebook<https://mandrillapp.com/track/click/30634852/www.facebook.com?p=eyJzIjoiaXBySTBMZ3QtZUJ6QngtSVg3X1RYRmpVbzZzIiwidiI6MSwicCI6IntcInVcIjozMDYzNDg1MixcInZcIjoxLFwidXJsXCI6XCJodHRwczpcXFwvXFxcL3d3dy5mYWNlYm9vay5jb21cXFwvRUNPaGFiaXRhdGlvblxcXC9cIixcImlkXCI6XCI1Zjc5MjFjMzE2ZjE0YzJjYjBkNGU5OGZlNmQzYmE4N1wiLFwidXJsX2lkc1wiOltcImVhOTZhYTFmMmQ1MzU4OGE5NzcwYjBkNWFiY2Y0MmRhNzhkYTEzODVcIl19In0> | twitter<https://mandrillapp.com/track/click/30634852/twitter.com?p=eyJzIjoiakdBeGxhNHpTMVc4THZtRjhQQ2ZRcmNBQThJIiwidiI6MSwicCI6IntcInVcIjozMDYzNDg1MixcInZcIjoxLFwidXJsXCI6XCJodHRwczpcXFwvXFxcL3R3aXR0ZXIuY29tXFxcL0Vjb2hhYml0YXRpb25cIixcImlkXCI6XCI1Zjc5MjFjMzE2ZjE0YzJjYjBkNGU5OGZlNmQzYmE4N1wiLFwidXJsX2lkc1wiOltcIjBiODcyNWZlYjFiNGQ4ZjkyNTQ4ODA2OGM5ZTQ4ZjE1MGMxM2JhY2ZcIl19In0> | infolettre<https://mandrillapp.com/track/click/30634852/www.ecohabitation.com?p=eyJzIjoiVkE1Z0RKMWg5bm5HWlZkRlNHVXhyd2UzaU5FIiwidiI6MSwicCI6IntcInVcIjozMDYzNDg1MixcInZcIjoxLFwidXJsXCI6XCJodHRwOlxcXC9cXFwvd3d3LmVjb2hhYml0YXRpb24uY29tXFxcL25ld3NsZXR0ZXJcXFwvYWJvbm5lbWVudC1idWxsZXRpbi1lY29oYWJpdGF0aW9uXCIsXCJpZFwiOlwiNWY3OTIxYzMxNmYxNGMyY2IwZDRlOThmZTZkM2JhODdcIixcInVybF9pZHNcIjpbXCJmY2UwMjc3MWRlOGEwMGM5NzcwY2E3YmU2ZGUzNWFkZWI2ODQzZWEwXCJdfSJ9>
Le jeu. 14 mars 2019 à 09:58, Kyle Anders via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> a écrit :
That's my interpretation, although I know of at least one local code (Ontario's SB-10) that has modified this:
[image.png]
On Thu, Mar 14, 2019 at 9:46 AM Chris Hadlock via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
Good morning,
This is a question for my follow Canadians that have experience with the NECB 2015 code.
What is everyone's take on what fenestration area to model for the reference model when the Proposed model area is less than the maximum permitted?
Specifically, I'm referring to Part 8.4.4.3.3) which states "If the total vertical fenestration and door area to gross wall area (FDWR) of the proposed building differs from the maximum permitted by Article 3.2.1.1., the FDWR of the reference building shall be adjusted proportionally along each orientation until it complies with that Article."
Do people interpret this as if my Proposed FDWR is say 20%, then my Reference FDWR is to be increased to say 40% (based on a Zone 5 climate)?
Thanks,
Chris
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<https://mandrillapp.com/track/click/30634852/lists.onebuilding.org?p=eyJzIjoiMTltd3RJZnpsN1VzQ3Vzb29NbE9LbDdWSEpZIiwidiI6MSwicCI6IntcInVcIjozMDYzNDg1MixcInZcIjoxLFwidXJsXCI6XCJodHRwOlxcXC9cXFwvbGlzdHMub25lYnVpbGRpbmcub3JnXFxcL2xpc3RpbmZvLmNnaVxcXC9lcXVlc3QtdXNlcnMtb25lYnVpbGRpbmcub3JnXCIsXCJpZFwiOlwiNWY3OTIxYzMxNmYxNGMyY2IwZDRlOThmZTZkM2JhODdcIixcInVybF9pZHNcIjpbXCI2MDE1NDNjZTMwMjRiYTI1MWNjNDM1Yzk2ZDhmY2M3ZmMzNWY4YjRlXCJdfSJ9>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
Kind Regards,
KYLE ANDERS, MASc, NRCan EA, LEED for Homes Green Rater
Senior Project Manager
T | 1-800-267-6830 x180 C | 226-220-2391
F | 519-658-6103 E | kyle at buildingknowledge.ca<mailto:kyle at buildingknowledge.ca>
This communication is intended for the sole use of the person(s) to whom it is addressed, and may contain information that is privileged, confidential or subject to copyright. Any unauthorized use, disclosure or copying of this communication is strictly prohibited. If you have received this communication in error, please contact the sender immediately. Any communication received in error should be deleted and all copies destroyed.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<https://mandrillapp.com/track/click/30634852/lists.onebuilding.org?p=eyJzIjoiMTltd3RJZnpsN1VzQ3Vzb29NbE9LbDdWSEpZIiwidiI6MSwicCI6IntcInVcIjozMDYzNDg1MixcInZcIjoxLFwidXJsXCI6XCJodHRwOlxcXC9cXFwvbGlzdHMub25lYnVpbGRpbmcub3JnXFxcL2xpc3RpbmZvLmNnaVxcXC9lcXVlc3QtdXNlcnMtb25lYnVpbGRpbmcub3JnXCIsXCJpZFwiOlwiNWY3OTIxYzMxNmYxNGMyY2IwZDRlOThmZTZkM2JhODdcIixcInVybF9pZHNcIjpbXCI2MDE1NDNjZTMwMjRiYTI1MWNjNDM1Yzk2ZDhmY2M3ZmMzNWY4YjRlXCJdfSJ9>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190314/1d363ffe/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 20854 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190314/1d363ffe/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 3859 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190314/1d363ffe/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 70848 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190314/1d363ffe/attachment.png>
More information about the Equest-users
mailing list