[Equest-users] HVAC pump with 11 W/gpm
David Eldridge
DEldridge at grummanbutkus.com
Tue Mar 12 11:57:31 PDT 2019
It’s a trade-off, the limit is prescribed for the baseline model but the proposed design may pump horsepower that is called for in the design – however if you go above the limit then there will have to be some corresponding efficiency to trade-off the net effect of the pump power.
For your particular project given some constraints it may not be possible to vary pipe size, layout, and •T enough to achieve the limit – that’s okay if the modeling will still show net project savings from control of the pumping system and other energy efficiency measures in the project.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Associate
Direct: (847) 316-9224 | Mobile: (773) 490-5038
Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201
Energy Efficiency Consultants and Sustainable Design Engineers
grummanbutkus.com<http://grummanbutkus.com/> | Blog<http://grummanbutkus.com/blog> | Facebook<https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526> | Twitter<https://twitter.com/grummanbutkus>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Dante Garcia via Equest-users
Sent: Thursday, March 07, 2019 2:57 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] HVAC pump with 11 W/gpm
Hello,
I have a general question redargin how to design HVAC pump with 11 W/gpm per primary and secondary loops in evaporator.
Please advise how a design can achieve that target. Most design that I have seen exceeds that limits becasuse it does not consider head.
Regards,
Dante
--
SUMAC
Dante Garcia // LEED AP BD+C
dgarcia at sumacinc.com<mailto:dgarcia at sumacinc.com>
www.sumacinc.com
<http://www.sumacinc.com/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190312/a3d3b3a4/attachment.html>
More information about the Equest-users
mailing list