[Equest-users] eQuest VRF question
Matthew S. Garlick
msg at tbcxinc.com
Fri Mar 15 14:09:27 PDT 2019
Christopher,
I was hoping someone else would chime in on this since it's the question I'm asking as well! Working with Mitsubishi a few months back, I got the following:
"In eQUEST, you can model water-source VRF as a standard WSHP and then choose the option for staged or multi speed compressor to approximate the performance of an inverter compressor. Using standard WSHP definitions in eQUEST will not be far off from water-source VRF operation since water-source equipment isn't subject to the capacity de-rates air-source VRF is subject to, so essentially the variable speed nature of the compressor is the only thing that is missing to properly model water-source VRF.
Additionally, in eQUEST the EIR (energy input ratio - described in the first attachment) has an overwhelming impact on the resulting energy performance - much more so than the capacity and part-load curves. Since the EIR is calculated and entered for each specific condenser being modeled, this should reflect water-source VRF operation with a reasonable degree of accuracy.
We could update the attached white paper and associated eQUEST curves to include water-source VRF, however, most open source energy modeling is now trending toward Energy Plus and the various interfaces that run this engine like OpenStudio."
Talking to Doug Maddox who helped develop the air source VRF in DOE 2.3, he said he thought that approach is reasonable.
Please let me know if you find anything else, I've got a big water source VRF model in my near future!
Best,
[TBCx]
Matt Garlick, CxA, CEM, BEMP
Building Efficiency Engineer | TBCx
E-mail: msg at tbcxinc.com<mailto:msg at tbcxinc.com>
Mobile: 801-907-5654
Direct: 801-401-8456
324 S. State Street, Suite 400
Salt Lake City, UT 84111
www.tbcxinc.com<http://tbcxinc.com/>
From: Jones, Christopher <Christopher.r.Jones at wsp.com>
Sent: Thursday, March 14, 2019 7:22 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] eQuest VRF question
Is it possible to model a water-source VRF system? Typically these systems have a source/sink water loop similar to a water-source heat pump loop with a boiler and fluid cooler. I did RTFM and it appears that only an air cooled condenser is available for the VRF system at this time.
In the past, I used the water-source heat pump system to approximate a water-source VRF system. It looks like I will have to use that strategy with DOE2.3.
Christopher R. Jones, P.Eng.
Senior Building Performance Specialist
Sustainability & Energy
[cid:image001.png at 01D4DB41.1489F650]
T+ 1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190315/974c3aa3/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 1860 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190315/974c3aa3/attachment-0003.png>
More information about the Equest-users
mailing list