[Equest-users] eQuest Fan Curve Question
Nicholas Caton
Nicholas.Caton at se.com
Fri Jun 28 08:39:44 PDT 2019
Hi Kirk,
This is a common enough issue that I think it merits repeating for the [equest-users] community - I hope you don't mind my CC'ing them here.
That particular fan curve ("Variable Speed Drive FPLR") has a storied history of throwing this particular caution. Commonly the the very first or last hour of the simulation is flagged (noting in your example below, 12/31/24 below infers the hour containing everyone's new-year's countdown).
I think there's consensus among the community that this is one of a family of cautions/warnings which you can safely ignore as erroneous.
~Nick
[cid:image005.png at 01D515A3.47EDD880]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Energy Performance Contracting
D
M
F
E
913 . 564 . 6361
785 . 410 . 3317
913 . 564 . 6380
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image006.png at 01D515A3.47EDD880]
From: Kirk Plum <kplum at bhbinc.com>
Sent: Wednesday, June 26, 2019 4:57 PM
To: Nicholas Caton <Nicholas.Caton at se.com>
Subject: eQuest Fan Curve Question
Nick,
I appreciate the help earlier! I was wondering if you have ever gotten this error message?
**CAUTION**********************************************************************
In curve: Variable Speed Drive FPLR the dependent value
is exceeding the limits.
Value/Min/Max/First time: 1.257 0.100 1.000 12/31/24
I tried looking at the fan curves, but I do not have any experience in editing these in eQuest. I appreciate any help!
Thanks,
Kirk Plum, EIT, LEED Green Associate
Graduate Mechanical Engineer
Baird, Hampton & Brown
6300 Ridglea Place, Suite 700
Fort Worth, Texas 76116
817.338.1277 phone
kplum at bhbinc.com<mailto:kplum at bhbinc.com>
TBPE Firm #44 | TBPLS Firm #10011300 #10011302 #10194146
bhbinc.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.bhbinc.com%2F&data=02%7C01%7Cnicholas.caton%40se.com%7Ce7d30588fb0742262c1908d6fa814cb8%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C1%7C636971830589807178&sdata=VmOrrZTaKo%2FoyvznZB2Hu7oPDCCduOwTzn8y8IluXY0%3D&reserved=0> | LinkedIn<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.linkedin.com%2Fcompany%2Fbaird-hampton-and-brown-inc.&data=02%7C01%7Cnicholas.caton%40se.com%7Ce7d30588fb0742262c1908d6fa814cb8%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636971830589817172&sdata=zinIOHBpXegb8DptkiWfaSSSVDn%2BFmBHg6JtXrNWBJo%3D&reserved=0> | Facebook<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fbhbinc%2F&data=02%7C01%7Cnicholas.caton%40se.com%7Ce7d30588fb0742262c1908d6fa814cb8%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636971830589817172&sdata=t%2BoKl%2FWD0ll4bP6lYgIAEIub0EBMvz3xoYKZWUPBlxc%3D&reserved=0>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190628/5181e0aa/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190628/5181e0aa/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190628/5181e0aa/attachment-0001.png>
More information about the Equest-users
mailing list