Nick,
I'm glad that Erik took the first shot in answering your question, as I
was leery to say too much because I haven't followed the development of
DOE-2.2 much at all and might be giving you outdated impressions from
DOE-2.1E. However, your question seems to ask a generic question of
why the design capacities in the verification reports (SV-A, PV-A, etc.)
differ from the peak loads in the simulation reports (SS-H, PS-H,
etc.). Design capacities are either input by the user or calculated
using design day conditions which are worse-case conditions, i.e.,
weather conditions at the 0.4% criteria and the building at full
operations for all zones (this is for cooling; for heating the building
is assumed to be completely off except for the HVAC). I apologize if
that's all well known, in which case take this as an extended hello
prior to meeting in KC!
Joe
On 6/13/2019 11:08 AM, Erik Kolderup via Equest-users wrote:
> Hi, Nick.
>
> I think that the capacity of the cooling loop will be based on the sum
> of the capacities of cooling coils connected to the loop, assuming the
> sizing option for the loop is "secondary" rather than "primary". If
> you look at the SV-A report and sum up capacity of all the cooling
> coils, does that get you to 13 MBtu/hr? If you want the loop sized
> based on chiller size, then the sizing option for the loop should be
> "primary".
>
> -Erik
>
>
> *Erik Kolderup, PE, LEED AP*
> erik at kolderupconsulting.com <mailto:erik at kolderupconsulting.com>|
> 415.531.5198 | www.kolderupconsulting.com
> <http://www.kolderupconsulting.com>
>
>
> On Thu, Jun 13, 2019 at 11:02 AM Nicholas Caton via Equest-users
> <equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>> wrote:
>
> Hi everyone,
>
> Can anyone help me assert or correct my understanding on
> something? This is from a model built in v3.65, b7175, doe2.2
> engine (with intent to upconvert the project to doe2.3 before I’m
> done).
>
> Report PV-A lists the capacity for each heating/cooling loop.
> Here I’m cropping to just the loops, and highlighting what I’m
> used to thinking of as the “peak” coincident capacity requirement
> for a chilled water loop – 13.909 MMBtu/hr (that’s millions):
>
> The following reports PS-H go into more detail on each item listed
> in PV-A. Here is the report for the same “Chilled Water Loop,”
> with a coule more highlights:
>
> Immediately, I note that *13.909 MMBtu/hr*(1,159 tons) aligns with
> PV-A, however I do not see that number matching (intuitively) any
> of the other figures or sums provided on this sheet. The figure
> 5,625.126 kBtu/hr (469 tons) aligns with my expectations for peak
> load on the loop, where nominal capacity of the associated
> chillers on this loop are in the same ballpark (one is 444 tons
> and one is 210 tons on paper & @ design conditions, and I’m told
> they commonly do not need to engage the smaller chiller during the
> dead of summer).
>
> Can anyone help me reconcile the differences between what’s
> reported as “Cooling Capacity” in PV-A, in relation to the annual
> peak loads indicated for the same loop in the PS-H report?
>
> Thanks!
>
> ~Nick
>
> cid:image005.png at 01D515A3.47EDD880
>
> *Nick Caton, P.E., BEMP*
>
> Senior Energy Engineer
> Regional Energy Engineering Manager
>
> Energy and Sustainability Services
> Energy Performance Contracting
>
>
>
> D
> M
> F
> E
>
>
>
> 913 . 564 . 6361
>
> 785 . 410 . 3317
>
> 913 . 564 . 6380
>
> _nicholas.caton at se.com <mailto:nicholas.caton at se.com>_
>
>
>
> 15200 Santa Fe Trail Drive
> Suite 204
> Lenexa, KS 66219
> United States
>
> cid:image006.png at 01D515A3.47EDD880
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190613/1c0816ab/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 44782 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190613/1c0816ab/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 306303 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190613/1c0816ab/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190613/1c0816ab/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190613/1c0816ab/attachment-0002.png>
More information about the Equest-users
mailing list