Nicholas Caton
Nicholas.Caton at se.com
Thu Jun 27 15:43:41 PDT 2019
Hi Victoria,
This sounds like a good case for utilizing the doe 2.3 engine with the most recent build. I think this will allow you to essentially model your AHU's as describes as a DOAS, and then to have them "attach" to another airside system which could explicitly simulate the operations of your unit heaters.
You would specify DOAS-ATTACHED-TO as CONDITIONED-ZONES to replicate the situation where the two systems are not directly piping air between each other, but instead draw separately from the mixed air of the conditioned space. You might review the reference entry for DOAS-ATTACHED-TO to see if that prompts you to consider defining a gym 'plenum' in further consideration of where these different units exist on the z-axis, in the event it isn't likely the whole volume is 'perfectly mixed.'
One thought: You might not be able to select and attach a system of type UH to a DOAS, considering UH by it's doe2 definition doesn't permit the introduction of ventilation air, but it may be worth a shot. If that doesn't work, you could likely define any number of other systems which permit the simple definition of a fan, heating coil, and ventilation air (multiple ways to skin the cat there).
~Nick
[cid:image005.png at 01D515A3.47EDD880]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Energy Performance Contracting
D
M
F
E
913 . 564 . 6361
785 . 410 . 3317
913 . 564 . 6380
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image006.png at 01D515A3.47EDD880]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Civitillo, Victoria via Equest-users
Sent: Wednesday, June 26, 2019 11:14 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Unit Heaters and RTUs serving the same zone
[External email: Use caution with links and attachments]
________________________________
Hi all,
I am in the process of modeling a gymnasium that is served by two system types and I'm looking for the best way to model it. RTUs serve the space for cooling and ventilation purposes while hot water unit heaters supply the heating. The ventilation air from the RTUs tempered to 65degF during the heating months. Trying to figure out if there is a way to model it as a single system? I originally thought I could just mimic the RTU heating coil as the unit heater heating coil but got a ton of unmet hours. I have taken a powered induction unit with preheat as the approach now which has nixed my unmet hours but skyrocketed my heating energy consumption. Open to suggestions!
Thanks in advance,
Victoria
Victoria (Tsamis) Civitillo, PE, CEM, LEED AP BD+C, WELL AP
Sustainability Project Manager
Direct: (212) 330-6165
Stantec Consulting Services Inc.
475 Fifth Avenue 12th Floor
New York NY 10017-7239 US
[Stantec]<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.stantec.com%2F&data=02%7C01%7CNicholas.Caton%40se.com%7C7129c65bc78e4615933b08d6fa515e99%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636971624723307050&sdata=7VerpCeUWsKpYcF8Ca9dKqqZzJzHcxWhLCZh5xOE5Yg%3D&reserved=0>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
? Please consider the environment before printing this email
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190627/08b7bdb6/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190627/08b7bdb6/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190627/08b7bdb6/attachment-0007.png>
More information about the Equest-users
mailing list