[Equest-users] Does anyone know if eQuest can model this system??

Bishop, Bill bbishop at pathfinder-ea.com
Mon Jul 8 12:52:10 PDT 2019


Hi John,
There is a chiller with TYPE=WATER-ECONOMIZER but it looks like there has to be another actual chiller attached to the loop for it to work. You could model a very small mechanical chiller along with a water-economizer chiller, with both chillers attached to a condensing loop served by a cooling tower. You will probably get a high number of unmet cooling hours unless the FCUs never see much of a cooling load.

~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer

[Pathfinder-EA-logo-2]T: (585) 698-1956                        F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>        www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608               [cid:image003.png at 01D535A5.59BB70F0]         Ask me why Carbon Fee & Dividend may be right for you.

From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of John Aulbach via Equest-users
Sent: Sunday, July 7, 2019 10:06 PM
To: equest-users at onebuilding.org
Subject: [Equest-users] Does anyone know if eQuest can model this system??

2-Pipe fan coils. Heating source is hot water from boiler. Cooling source is condenser water fro cooling tower. All converted from a water source heat pump.

Thanks,

John R. Aulbach, PE
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190708/86d6571e/attachment-0001.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190708/86d6571e/attachment-0002.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 1554 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190708/86d6571e/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 1903 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190708/86d6571e/attachment-0003.jpg>


More information about the Equest-users mailing list