Konstantina,
You are correct to model VAV systems with parallel and series powered boxes as PIU system type.
This system type will enable several keywords at the zone level on the Airflow tab:
[cid:image003.png at 01D546B7.A30B1670]
Included in these is ZONE-FAN-RATIO and ZONE-FAN-KW/FLOW where you can enter your VAV box fan power.
Footprint
Brian Fountain
Associate
d 416 572 8501 m 416 562 6831
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Konstantina Kalliakoudi via Equest-users
Sent: Tuesday, July 30, 2019 8:44 AM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] Modeling Ashrae - System 8 in equest - Fan in the parallel box
CAUTION: EXTERNAL SENDER
Dear equest users,
According G3.1.3.14 for system 8 the fan parallel box shall be modeled with 0.35 W/cfm fan power.
I was wondering where this paramater can be insered in equest.
In the following screenshot I have input the power of the supply fan.
[image.png]
Thank you very much.
Best regards
[https://ssl.gstatic.com/ui/v1/icons/mail/images/cleardot.gif]
Konstantina Kalliakoudi
Mechanical Engineer Μ.Sc.
www.khmoe.gr<http://www.khmoe.gr/>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190730/751d48f3/attachment.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 93259 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190730/751d48f3/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 87195 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190730/751d48f3/attachment-0005.png>
    
    
More information about the Equest-users
mailing list