[Equest-users] High pumps equivalent full load hours in the model
Nicholas Caton
Nicholas.Caton at schneider-electric.com
Mon Jan 28 13:04:51 PST 2019
@David Eldridge, Bill Bishop, & Kathryn Kerns: Thank you for your immediate/parallel responses! That’s exactly the sort of discussion & feedback I was hoping to spark and for all of us to learn from.
I am a couple years distanced today from when I was breathing LEED 365 days/yr as an independent consultant, so I’m keen to keep a pulse on how the standards and rating systems of the day continue to push the envelope forward on systems engineers and designers.
I feel the first decade+ of my career was focused on learning to design & specify ever more complex systems and operations. My more recent years have exposed me to repeated cases of “death by complexity” however, and so I’m bearing back a bit towards questioning the value of some such decisions. In broad terms, I think well-meaning and intelligent engineers can often fall into the trap of designing fighter jets for cab drivers. Sometimes the most correct energy solution on paper misses the end-users and operators who will make or (emphasis) break the realized savings. Learning to balance the optimal level of design and operation complexity is an area of focus for me these days.
Kind regards,
~Nick
[cid:image001.png at 01D4B4C4.B39827B0]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D4B4C4.B39827B0]
From: David Eldridge <DEldridge at grummanbutkus.com>
Sent: Friday, January 25, 2019 2:39 PM
To: Nicholas Caton <Nicholas.Caton at schneider-electric.com>; Chapin, Alex N <Alex.Chapin at masonandhanger.com>; Morteza Kasmai <morteza.kasmai at gmail.com>; equest-users at onebuilding.org
Subject: RE: [Equest-users] High pumps equivalent full load hours in the model
________________________________
Nick, nothing precluded in the proposed case – these aren’t from the mandatory section – however the baseline is supposed to include the applicable energy efficiency measures as you’ve described. I think you (Morteza) should follow up with Alex’s comments about how the building is divided and baseline systems assigned.
EFLH means running at full capacity though, so although this system may need to be available year-round or nearly year-round, why aren’t some portions of it closing down? In a nutshell – I’m not sure the system selection is correct and you may be able to make an end-run on the issue altogether. I unfortunately don’t have time to dig through the model files (or even verify which version of 90.1 is being discussed), but the setup is not typical for what I’m seeing in practice now (LEED, Green Globes, or not certified), and also not knowing the areas of all these components entering the system selection matrix.
I agree with Alex’s point that the corridor system would be separate in the system selection from the retail, and also the residential units. The typical setup that we’d see in this case is a make-up air unit, potentially DX, and which according to many building codes supplies the same volume of 100% outside air at all times to make up the kitchen (hopefully…), in-unit clothes dryer if applicable, and bathroom exhausts. It could vary airflow if the exhaust air from the apartments was known to vary. To Nick’s point – that’s a complicated system for a baseline. For the most advanced energy efficiency cases, perhaps a DOAS unit with heat recovery. (One clue would be does the proposed building also have a DOAS that serves only the apartment stack?) PTAC per floor for corridor area might also be justifiable.
Then the retail unit would be separate – besides different operating schedule the tenant would pay for their own utilities so it is not likely to be combined with the corridor AHU on a hydronic system. Only in the largest buildings would these end up being hydronic systems with submetering. This will most likely be its own DX VAV or maybe CHW system, it should have its own outside air supply pathway, etc.
David
David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
Associate
Direct: (847) 316-9224 | Mobile: (773) 490-5038
Grumman/Butkus Associates | 820 Davis Street, Suite 300 | Evanston, IL 60201
Energy Efficiency Consultants and Sustainable Design Engineers
grummanbutkus.com<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fgrummanbutkus.com%2F&data=02%7C01%7CNicholas.Caton%40schneider-electric.com%7Ce8046a7b74b4463348e108d6830534cd%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636840455727464157&sdata=Jj3utoz8Eh0a35mWxz9Uwbg10L1lNBlVOzPrhcukej0%3D&reserved=0> | Blog<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fgrummanbutkus.com%2Fblog&data=02%7C01%7CNicholas.Caton%40schneider-electric.com%7Ce8046a7b74b4463348e108d6830534cd%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636840455727464157&sdata=jAVRRTTrN7A5N%2Ft5EtJLsvQ83tZBG4HX6wcBoiIcAOg%3D&reserved=0> | Facebook<https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.facebook.com%2Fpages%2FGrummanButkus-Associates%2F1385285015032526&data=02%7C01%7CNicholas.Caton%40schneider-electric.com%7Ce8046a7b74b4463348e108d6830534cd%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636840455727474170&sdata=xFD1KeyXD0zAHnjgZM292R1IDYxcE60D3ukYm5qe3xU%3D&reserved=0> | Twitter<https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Ftwitter.com%2Fgrummanbutkus&data=02%7C01%7CNicholas.Caton%40schneider-electric.com%7Ce8046a7b74b4463348e108d6830534cd%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636840455727484178&sdata=65oO10G7pWWGk1DGzR3KRXVBQODMoDxwKoYsoCD5Es0%3D&reserved=0>
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton via Equest-users
Sent: Friday, January 25, 2019 12:51 PM
To: Chapin, Alex N <Alex.Chapin at masonandhanger.com<mailto:Alex.Chapin at masonandhanger.com>>; Morteza Kasmai <morteza.kasmai at gmail.com<mailto:morteza.kasmai at gmail.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] High pumps equivalent full load hours in the model
Not to make this more difficult than necessary, but could I take a step back and ask: Can anyone comment regarding what exactly between LEED and/or 90.1 precludes 24/7 hydronic loop circulation?
This is NOT an uncommon control scheme to encounter in the real world, and the inherent simplicity of 24/7, constant-speed operations carry some real advantages with respect to system first-cost, simplicity / troubleshooting, and maintenance over time.
That’s not to say variable flow pumps, demand based on/off controls, and other schemes are a bad idea (I’m regularly implementing such strategies where it pencils out), but I’ve encountered a number of cases where variable-flow upgrades implemented badly can end up causing more harm ($$$/downtime) than good.
I am left sincerely interested to learn and understand what exactly the LEED reviewers may be expecting/requiring of hydronic system pumping operations.
Thanks,
~Nick
[cid:image001.png at 01D4B19C.3EADA950]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D4B19C.3EADA950]
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Chapin, Alex N via Equest-users
Sent: Monday, January 21, 2019 7:14 AM
To: Morteza Kasmai <morteza.kasmai at gmail.com<mailto:morteza.kasmai at gmail.com>>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] High pumps equivalent full load hours in the model
[External email: Use caution with links and attachments]
________________________________
Hi Morteza,
I looked at the file quickly and it seems that there are some changes that you can make to reduce the EFLHs slightly (I was able to get it to 8,146 hours/year by changing to two-way HW and CHW coils, moving cooling coils to secondary loop, readjusting pump flows and power after other changes, and setting loop operation to demand), but it seems like the underlying cause of the high EFLHs is probably due to having VAV systems which only serve interior spaces which are probably going to be in cooling mode year round.
Note that I think you can model the corridors on floors with residential as PTACs also. I believe that the reviewer should allow you to be flexible in how you define the corridor off of residential spaces. This might help reduce the pump EFLHs for primary and secondary chilled water pumps, assuming those VAVs which only serve core spaces are part of what is driving the high EFLHs.
Alex Chapin EIT, BEMP, LEED AP BD+C, O+M
Energy Engineer | Mason & Hanger
A Day & Zimmermann Company
D 804.521.7072 | O 804.285.4171 | F 804.217.8520
4880 Sadler Road, Suite 300 | Glen Allen, VA 23060
masonandhanger.com<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.masonandhanger.com%2F&data=02%7C01%7CNicholas.Caton%40schneider-electric.com%7Ce8046a7b74b4463348e108d6830534cd%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636840455727484178&sdata=93sK%2Fz0rvKYlWo36o7q%2B8ZtqiciZ7Au%2BZ09NY6fZlFQ%3D&reserved=0>
Building a More Secure World
From: Morteza Kasmai <morteza.kasmai at gmail.com<mailto:morteza.kasmai at gmail.com>>
Sent: Friday, January 18, 2019 1:29 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] High pumps equivalent full load hours in the model
Hello all,
I received following LEED review comment:
“The Baseline model pumps equivalent full load hours (determined by dividing the total annual pumps consumption (45,761 KWH) by the pump peak demand (5.426 KW) reflected in the simulation output report) is 8,433 hours/year, which is unexpectedly high given the anticipated schedule of operation for the project.”
This is a 9 story residential building with unfinished retail space in the ground floor. Primary HVAC system in the baseline case is PTAC and the secondary system that serves non-residential spaces is System 7 – VAV with reheat and chilled water. HVAC system in unfinished retail space of the propose model is System 7 as well. Pumps equivalent full load hours for the proposed model is 8,089 hours/year (15,401/1.905), which is close to EFLH of the baseline case.
Is this high EFLH loads relate to the primary and secondary pumps in both of the models and are justifiable or there is something wrong with the models. Attached are inp and pd2 files of the baseline model from version 3.65 build 7173.
Thank you for your help,
Morteza Kasmaei
Senior Architect
LEED AP BD+C, GGP
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190128/de8aef67/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190128/de8aef67/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190128/de8aef67/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7137 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190128/de8aef67/attachment.obj>
More information about the Equest-users
mailing list