[Equest-users] VRF Question

Juan Carlos Sanabria Fallas juan.sanabria.fallas at jci.com
Fri Jan 18 07:37:40 PST 2019


Thanks Bill, that's work.

Best Regards,
Juan

Juan Carlos Sanabria
Sustainability Department Project Engineer
Circuito

Main:    +506 2243-1000
Direct:  +506 2243-1069
juan.sanabria.fallas at jci.com<mailto:juan.sanabria.fallas at jci.com>
www.johnsoncontrols.com<http://www.johnsoncontrols.com/>

Parque Empresarial Forum 1, Edificio H, Piso 2
San José, Costa Rica

THIS MESSAGE MAY CONTAIN INFORMATION THAT IS PRIVILEGED AND CONFIDENTIAL. The information contained in, or attached to, this message is intended solely for the use of the specific person(s) named above. If you are not the intended recipient then you have received this communication in error and are prohibited from review, retransmission, taking any action in reliance upon, sharing the content of, disseminating or copying this message and any of the attachments in any way. If you have received this communication in error, please contact the sender immediately and promptly delete this message from all types of media and devices. Thank you.

Please consider the environment before printing this message


From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Friday, January 18, 2019 8:43 AM
To: Juan Carlos Sanabria Fallas <juan.sanabria.fallas at jci.com>; Mirko Slivar <mirko.slivar at rpeng.ca>; David García <dgandres at hotmail.com>
Cc: equest-users at lists.onebuilding.org
Subject: RE: [Equest-users] VRF Question

Hi Juan,
Go to Tools -> Select DOE2 Version (At Next eQUEST Startup) ->
and select DOE 2.3.
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer

[Pathfinder-EA-logo-2]T: (585) 698-1956                        F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>        www.pathfinder-ea.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.pathfinder-ea.com%2F&data=02%7C01%7Cjuan.sanabria.fallas%40jci.com%7C9bb3c442d4bb4fa763f808d67d535762%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C636834194243080223&sdata=8CKKb2oNUfpmbcmcxAuxNJ7GSkV%2B%2FOVhCm9DZZ%2B7i9A%3D&reserved=0>
134 South Fitzhugh Street
Rochester, NY 14608               [cid:image002.png at 01D4AF11.718B0CB0]         Ask me why Carbon Fee & Dividend may be right for you.

From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Juan Carlos Sanabria Fallas via Equest-users
Sent: Friday, January 18, 2019 9:33 AM
To: Mirko Slivar <mirko.slivar at rpeng.ca<mailto:mirko.slivar at rpeng.ca>>; David García <dgandres at hotmail.com<mailto:dgandres at hotmail.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] VRF Question

Hi, sorry but didn't appear for me

[cid:image003.jpg at 01D4AF11.718B0CB0]

Someone know why?

Juan Carlos Sanabria
Sustainability Department Project Engineer
Circuito

Main:    +506 2243-1000
Direct:  +506 2243-1069
juan.sanabria.fallas at jci.com<mailto:juan.sanabria.fallas at jci.com>
www.johnsoncontrols.com<https://na01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.johnsoncontrols.com%2F&data=02%7C01%7Cjuan.sanabria.fallas%40jci.com%7C9bb3c442d4bb4fa763f808d67d535762%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C636834194243080223&sdata=N%2FCa0HegtRhYZx9kxeM0rKGCV3GeoghGbV5q2tbPHrQ%3D&reserved=0>

Parque Empresarial Forum 1, Edificio H, Piso 2
San José, Costa Rica

THIS MESSAGE MAY CONTAIN INFORMATION THAT IS PRIVILEGED AND CONFIDENTIAL. The information contained in, or attached to, this message is intended solely for the use of the specific person(s) named above. If you are not the intended recipient then you have received this communication in error and are prohibited from review, retransmission, taking any action in reliance upon, sharing the content of, disseminating or copying this message and any of the attachments in any way. If you have received this communication in error, please contact the sender immediately and promptly delete this message from all types of media and devices. Thank you.

Please consider the environment before printing this message


From: Mirko Slivar [mailto:mirko.slivar at rpeng.ca]
Sent: Sunday, January 13, 2019 10:13 AM
To: David García <dgandres at hotmail.com<mailto:dgandres at hotmail.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] VRF Question

Thanks David
I got it to work.
Mirko Slivar, P. Eng.
Principal
Cell: (250) 859-3470
Sent from my iPhone

On Jan 13, 2019, at 5:11 AM, David García <dgandres at hotmail.com<mailto:dgandres at hotmail.com>> wrote:
Hi all,

Following Doug Maddox's webinar you can find VRF System using DOE 2.3 as follows:

<image001.png>


David García
MEP Senior Engineer. Parksmart Advisor.
Sustainability Consultant. Energy Modeler.
Mobile: +34 638 01 87 95
dgandres at hotmail.com<mailto:dgandres at hotmail.com>
Madrid, SPAIN


-----Mensaje original-----
De: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> En nombre de Paul Diglio via Equest-users
Enviado el: domingo, 13 de enero de 2019 13:35
Para: Mirko Slivar <mirko.slivar at rpeng.ca<mailto:mirko.slivar at rpeng.ca>>; Hala Jaber <halajaber82 at gmail.com<mailto:halajaber82 at gmail.com>>
CC: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Asunto: Re: [Equest-users] VRF Question



I believe you need to choose a PVVT system for the VRF options to appear.



Paul Diglio

87 Fairmont Avenue

New Haven, CT  06513



--------------------------------------------

On Sun, 1/13/19, Hala Jaber via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:



Subject: Re: [Equest-users] VRF Question

To: "Mirko Slivar" <mirko.slivar at rpeng.ca<mailto:mirko.slivar at rpeng.ca>>

Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>

Date: Sunday, January 13, 2019, 12:39 AM

 Hi Mirko,

You have to use DOE 2.3 from:

tools ,select doe version then click on doe 2.3 then close

the equest and open it again.Good

luck.--

Best Regards,Hala Jaber.Sustainable Design Engineer.; LEED AP BD +C

,GSAS CGP,CMVP,CLEP.

 On Sat, 12 Jan

2019, 11:36 pm Mirko Slivar via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>

wrote:











 Hello,

A colleague and myself are both having the same issue.

We are running version 3.65 build 7175. With regards to the

new VRF system type neither of us can get this system type

option to appear on the system type pull down menu. We

choose DX coils for both

  the cooling and heating source but VRF is not listed as an

option under system type. Has anyone experienced this

?

Thanks

Mirko





 _______________________________________________

 Equest-users mailing list

 https://eur04.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7C%7Cb325da14250845a85b7f08d679538f5e%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636829797119201492&sdata=YxTe184JLAQ3oAILAa6zxgpJOWPqPSOm6PGlE2ZMhmU%3D&reserved=0<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Feur04.safelinks.protection.outlook.com%2F%3Furl%3Dhttp%253A%252F%252Flists.onebuilding.org%252Flistinfo.cgi%252Fequest-users-onebuilding.org%26data%3D02%257C01%257C%257Cb325da14250845a85b7f08d679538f5e%257C84df9e7fe9f640afb435aaaaaaaaaaaa%257C1%257C0%257C636829797119201492%26sdata%3DYxTe184JLAQ3oAILAa6zxgpJOWPqPSOm6PGlE2ZMhmU%253D%26reserved%3D0&data=02%7C01%7Cjuan.sanabria.fallas%40jci.com%7C9bb3c442d4bb4fa763f808d67d535762%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C636834194243080223&sdata=AQBUTJ7LwYmYRvmHKb%2FJj0YKlJJGw11iDPg%2FakESGQA%3D&reserved=0>

 To unsubscribe from this mailing list send  a blank message

to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

 _______________________________________________

Equest-users mailing list

https://eur04.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7C%7Cb325da14250845a85b7f08d679538f5e%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636829797119201492&sdata=YxTe184JLAQ3oAILAa6zxgpJOWPqPSOm6PGlE2ZMhmU%3D&reserved=0<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Feur04.safelinks.protection.outlook.com%2F%3Furl%3Dhttp%253A%252F%252Flists.onebuilding.org%252Flistinfo.cgi%252Fequest-users-onebuilding.org%26data%3D02%257C01%257C%257Cb325da14250845a85b7f08d679538f5e%257C84df9e7fe9f640afb435aaaaaaaaaaaa%257C1%257C0%257C636829797119201492%26sdata%3DYxTe184JLAQ3oAILAa6zxgpJOWPqPSOm6PGlE2ZMhmU%253D%26reserved%3D0&data=02%7C01%7Cjuan.sanabria.fallas%40jci.com%7C9bb3c442d4bb4fa763f808d67d535762%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C636834194243080223&sdata=AQBUTJ7LwYmYRvmHKb%2FJj0YKlJJGw11iDPg%2FakESGQA%3D&reserved=0>

To unsubscribe from this mailing list send  a

blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

 -----Inline Attachment Follows-----



_______________________________________________

Equest-users mailing list

https://eur04.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7C%7Cb325da14250845a85b7f08d679538f5e%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C636829797119201492&sdata=YxTe184JLAQ3oAILAa6zxgpJOWPqPSOm6PGlE2ZMhmU%3D&reserved=0<https://na01.safelinks.protection.outlook.com/?url=https%3A%2F%2Feur04.safelinks.protection.outlook.com%2F%3Furl%3Dhttp%253A%252F%252Flists.onebuilding.org%252Flistinfo.cgi%252Fequest-users-onebuilding.org%26data%3D02%257C01%257C%257Cb325da14250845a85b7f08d679538f5e%257C84df9e7fe9f640afb435aaaaaaaaaaaa%257C1%257C0%257C636829797119201492%26sdata%3DYxTe184JLAQ3oAILAa6zxgpJOWPqPSOm6PGlE2ZMhmU%253D%26reserved%3D0&data=02%7C01%7Cjuan.sanabria.fallas%40jci.com%7C9bb3c442d4bb4fa763f808d67d535762%7Ca1f1e2147ded45b681a19e8ae3459641%7C0%7C0%7C636834194243080223&sdata=AQBUTJ7LwYmYRvmHKb%2FJj0YKlJJGw11iDPg%2FakESGQA%3D&reserved=0>

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190118/92900308/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1903 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190118/92900308/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 1554 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190118/92900308/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 47809 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190118/92900308/attachment-0007.jpg>


More information about the Equest-users mailing list