[Equest-users] eQuest
Nicholas Caton
Nicholas.Caton at schneider-electric.com
Wed Jan 9 14:25:22 PST 2019
1. In terms of terminology while working in doe2/equest, I’d further reinforce for a smooth learning curve that as a truism in the “doe2 world,” there shall always be 1 space for every zone and 1 zone for every space. No more, no less. SPACEs and ZONEs accomplish different things, but they’re normally paired together on a 1-for-1 basis.
The end user has every flexibility however to split up a single designed space into multiple “zones” (as may typically occur when you have VAV boxes serving perimeter vs. core areas in an open office, for example), or conversely you have the option of combining multiple spaces/zones in the design into one larger space/zone for the purposes of simplifying your energy model. The power/decision is in your hands!
1. This may be different today as it has now been ~3 years since my last LEED submission and we’ve seen a couple substantial updates to the platform, but I think especially when starting out with eQuest as a new end-user, you might be best advised to avoid the LEED compliance skillset unless your hand is forced, as it introduces a host of potential tripping points (potential for user error and just plain bugginess) and new inputs that are in whole not required to develop a solid and rigorous energy model for LEED submission… then again this ruleset may have evolved in clarity/stability in recent years so I’ll defer to anyone else with more current experience.
Hope this is helpful!
~Nick
[cid:image001.png at 01D4A68B.B9087070]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D4A68B.B9087070]
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Bruce Easterbrook via Equest-users
Sent: Sunday, January 06, 2019 11:02 AM
To: lukman at sthw.org<mailto:lukman at sthw.org>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] eQuest
[External email: Use caution with links and attachments]
________________________________
On item 1 and the way you have input your data a space and a zone are the same. I use a CAD dwg for input of the floors. I normally input most of the rooms and corridors (spaces). Later when you do the zones you can group similar spaces into a zone.
There are a lot of discussions on this in the email archives. Try my name as author, at least 3 years old. It is not as simple as it sounds. There are lots of tiny things to trip you up. Always do lots of backups and always have one in reserve. Stay in the SD wizard until it runs the way you want. Fine tune the windows at this point. Before that leave them as basic areas.
Bruce Easterbrook P.Eng.
Abode Engineering
On 1/6/2019 6:55 AM, lukman via Equest-users wrote:
Hi eQuest users,
I am new to eQuest software, I have the following doubts
1. In SD/DD wizard 2nd page ( building foot print ) we are creating zones. After the wizard edit when taking spaces from building shell we getting the same area as zone. This means every zone have only one space?
2. When selecting code as Leed in first page , in space properties total area is dividing into all active areas. This is only for occupancy ?
[cid:image003.jpg at 01D4A68B.B9087070]
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7Cf5a65827744d40e4992908d673f8aa70%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636823909182061123&sdata=TKhVkabnRaUSTUX559ZDdIslyM6nvYIptQDm0zoJLZw%3D&reserved=0>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190109/ee7cdacd/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190109/ee7cdacd/attachment-0006.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190109/ee7cdacd/attachment-0007.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 134742 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190109/ee7cdacd/attachment-0003.jpg>
More information about the Equest-users
mailing list