[Equest-users] User Expression referencing Zone at system level
Krystyniak, Patrick
patrick.krystyniak at stantec.com
Fri Apr 26 07:10:19 PDT 2019
Nick,
I agree that blatant automation can be a dangerous game; especially if someone does not understand how to arrive at the same values manually. I do see a potential value with automation to develop dynamic parameters within a model. In some cases, trying to develop a way to automate things is slower than just doing the math. In other cases, dynamic calculations can potentially save time after a significant design change down the road.
In this case, the fan powers will have to be input manually regardless!
Thanks for everyone's input
Patrick Krystyniak
(212) 330-6174
Stantec Consulting Services Inc.
475 Fifth Avenue 12th Floor
New York NY 10017-7239 US
[Stantec]<http://www.stantec.com/>
The content of this email is the confidential property of Stantec and should not be copied, modified, retransmitted, or used for any purpose except with Stantec's written authorization. If you are not the intended recipient, please delete all copies and notify us immediately.
From: Nicholas Caton <Nicholas.Caton at se.com>
Sent: Thursday, April 25, 2019 5:13 PM
To: Bishop, Bill <bbishop at pathfinder-ea.com>
Cc: equest-users at lists.onebuilding.org; Jones, Christopher <Christopher.r.Jones at wsp.com>; Krystyniak, Patrick <patrick.krystyniak at stantec.com>
Subject: RE: User Expression referencing Zone at system level
Everything from Bill and Chris is great input/advice.
To be contrarian and add a touch of mentorship philosophy, I'm just going to come out and say something I think others may (or should) be considering.
Sometimes automation is, all things considered, slower than just doing the math. It's my personal opinion (informed from a little experience) that system fan and circulation loop pump power inputs generally fall into that camp.
There are also very real dangers in allowing anyone who cannot demonstrably "do the math" to utilize such automation. Assuming everything works and proper training is provided, you might the risk of stunting their professional development and technical potential.
Some on this mailing list have achieved (and shown me!) some amazing feats around substantial automated energy model generation, and to the extent those of you have achieved something resembling a ROI for that time investment I have and always will applaud you, however I urge extreme caution for those considering such a deep dive effort on these philosophical grounds. For the same reasons, I would be hesitant to permit someone learning under my wing to leverage such automation before ensuring they know how to "kick the tires" and develop the inputs when the automation won't work/fit the situation.
As a corollary: If you need to document (i.e. spreadsheet) this math ANYWAY for something like LEED submission, then universally you're going to spend less time doing that once vs. automating it and then doing it manually anyway.
~Nick
[cid:image002.png at 01D4FC14.83F78810]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Energy Performance Contracting
D
M
F
E
913 . 564 . 6361
785 . 410 . 3317
913 . 564 . 6380
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image003.png at 01D4FC14.83F78810]
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Bishop, Bill via Equest-users
Sent: Thursday, April 25, 2019 11:05 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] FW: User Expression referencing Zone at system level
[External email: Use caution with links and attachments]
________________________________
Hi Patrick,
Like Christopher said, you can't reference children. There may be other ways to do what you're trying to do without referencing the zone ASSIGNED-FLOW.
HOWEVER, for single-zone systems that use the CONTROL-ZONE keyword, the control zone is a keyword of the local component (the system).
You can reference the ASSIGNED-FLOW (or other keywords) of a control zone accordingly:
#LR("CONTROL-ZONE","ASSIGNED-FLOW")
If you knew, for example, that all your systems have 300 watts of fan power, you could enter this expression for SYSTEM:SUPPLY-KW/FLOW:
0.300/#LR("CONTROL-ZONE","ASSIGNED-FLOW")
This won't be as helpful in cases where you have more than one zone assigned to a single-zone system. And you'll probably want to make the expression more elaborate using an IF-THEN to account for cases where there is no assigned flow in the control zone.
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.pathfinder-ea.com%2F&data=02%7C01%7CNicholas.Caton%40se.com%7Ce9e5a3037e71498ae1d508d6c997ed7a%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636918051698290539&sdata=fzBTTRzyUdW6a5nCAksZDSPlTcaMNeEL9CNjXFQFitU%3D&reserved=0>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image006.png at 01D4FC14.83F78810] Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Jones, Christopher via Equest-users
Sent: Thursday, April 25, 2019 11:45 AM
To: Krystyniak, Patrick <patrick.krystyniak at stantec.com<mailto:patrick.krystyniak at stantec.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] User Expression referencing Zone at system level
I am not so sure you can reference children in the Keyword expressions. The DOE2.2 manual does not mention child referencing. I know you can reference child components using the Compliance Analysis modules - see the ComplianceAnalysis manual but not all those commands are available in the .inp Keyword expressions. For a single zone system, the SUPPLY-FLOW is the zone ASSIGNED-FLOW times the SIZING-RATIO. ASSIGNED-FLOW (times system SIZING-RATIO) in the zone takes precedence over supply flow keywords in the system. You might do testing querying the SYSTEM SUPPLY-FLOW with ASSIGNED-FLOW set in the zone and no system supply flow specified at the SYSTEM level.
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image001.png at 01D4FB5C.47A892E0]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Krystyniak, Patrick via Equest-users
Sent: Thursday, April 25, 2019 10:50 AM
To: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: [Equest-users] User Expression referencing Zone at system level
I am looking to utilize a user expressions that will calculate the kW/CFM for a given system. Each system is a single zone system.
Is it possible to reference the zone "Assigned-Flow" in a user expression at the system level?
I am unsure if you are able to reference a child component.. I receive an error trying something along the lines of #CR("ZONE","ASSIGNED-FLOW").
Thanks
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.wsp.com%2Fcasl&data=02%7C01%7CNicholas.Caton%40se.com%7Ce9e5a3037e71498ae1d508d6c997ed7a%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636918051698290539&sdata=U%2FkAfyymFHDvAHFsW3I3d4h8pkTJ1VSbsQEpWe1265w%3D&reserved=0>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.wsp.com%2Flcap&data=02%7C01%7CNicholas.Caton%40se.com%7Ce9e5a3037e71498ae1d508d6c997ed7a%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636918051698300551&sdata=aFSpRpIsTVUioUVj1RRC4aYYwtBfFSBfqEP74KABbHw%3D&reserved=0>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190426/9f812107/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 255 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190426/9f812107/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190426/9f812107/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image004.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190426/9f812107/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 1554 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190426/9f812107/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 1860 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190426/9f812107/attachment-0003.png>