[Equest-users] 2015 NECB Question, Intersecting Floor and Wall Area
Jones, Christopher
Christopher.r.Jones at wsp.com
Thu Apr 25 13:39:18 PDT 2019
Chris,
The NECB 2011 and 2015 assume that the Reference case envelope is perfect and that there are no penetrations of the insulation plane. For the Proposed case, both standards give you the 2% opt out clause – if the total penetrated area is less than/equal to the maximum of 2%, it can be ignored. If the area is greater than 2%, you need to calculate the effect of these penetrated areas on the overall wall R-value. The NECB 2017 mandates calculation of linear transition and point transition thermal bridges but still maintains that the Reference case envelope is perfect – unlike the BC Hydro assumption that applies an insulation derating factor to the Reference case effective insulation.
I did a calculation of the effect of balconies on a typical MURB with 5% total balcony slab edge are total wall area. The Shock balcony thermal break system would take over 20 years to payback – Toronto climate much longer in Vancouver. That is ignoring thermal comfort issues, potential condensation issues, etc.
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image001.png at 01D4FB85.6C641EF0]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Chris Hadlock via Equest-users
Sent: Thursday, April 25, 2019 12:02 PM
To: equest-users at lists.onebuilding.org
Subject: [Equest-users] 2015 NECB Question, Intersecting Floor and Wall Area
Good morning,
For you Canadians, I have a question about how to model the area where a floor slab intersects the exterior wall.
Specifically, Section 3.1.1.7.8) of the 2015 NECB says that "wall assemblies shall be considered to include all related structural framing and perimeter areas of intersecting interior walls but shall not include the perimeter areas where floor or roof slabs interrupt the wall's construction."
There is a reference to Note A-3.1.1.7.(8) which provides an illustration to depict the extent of the surface that is considered as a wall at the intersection with a floor. In this note, it also says "This Code may have different requirements for the perimeter area of floors."
Since I haven't seen any such requirements (how anyone else), I'm not sure how to treat this area.
When I have a building in which the insulating layer in the exterior wall assembly is intersected by the floor slab (thus breaking the insulation plane), I typically model my Proposed building with a separate assembly for the slab edge and assign a low R-value (reflective of a wall with no insulation).
My question then is, in this case, what would people model for the Reference model in terms of R-value at the slab edge (where the floor intersects the wall)?
As mentioned, I have not seen anything in NECB that specifically deals with the treatment of the slab edge (other than at grade level). Would the Reference model carry the same R-value as the Proposed model?
Thank you in advance for your input and thoughts.
Chris
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190425/fff3814f/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 1860 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190425/fff3814f/attachment.png>
More information about the Equest-users
mailing list