[Equest-users] How to setup interior walls with identical condition?
Nicholas Caton
Nicholas.Caton at se.com
Thu Apr 11 05:55:18 PDT 2019
If you can assert all other walls have conditioned spaces on the opposite side conditioned to similar temperatures, with similar load profiles to your tenant space, you can further assert there is no meaningful heat transfer to be modeled, in which case the simplest approach may be to just build a model with the wizards, then in detailed edits simply delete all exterior surfaces beyond the single curtain wall exposure. You may in doing so want to bump up the thermal mass in the “interior perimeter” spaces however to assure stability in heat transfer hour by hour.
There are also approaches to having the wizards generate interior walls for you for the appropriate sides – that involves definining perimeter zone spaces which deliberately do NOT line up with the shell footprint perimeter.
~Nick
[cid:image001.png at 01D4EFBA.D3BC1020]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Energy Performance Contracting
D
M
F
E
913 . 564 . 6361
785 . 410 . 3317
913 . 564 . 6380
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D4EFBA.D3BC1020]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Jing Hong via Equest-users
Sent: Wednesday, April 10, 2019 1:58 PM
To: equest-users at lists.onebuilding.org; equest-users at onebuilding.org
Subject: [Equest-users] How to setup interior walls with identical condition?
________________________________
Dear All,
I have a LEED ID project. It is a store with only one exterior curtain wall. How could I have all the other walls as interior walls with an identical condition?
Thank you,
Jing
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190411/da619dba/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190411/da619dba/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190411/da619dba/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7140 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190411/da619dba/attachment.obj>
More information about the Equest-users
mailing list