[Equest-users] Modeling ISMRE
Bishop, Bill
bbishop at pathfinder-ea.com
Fri Apr 5 11:39:09 PDT 2019
As if energy modeling wasn't difficult enough, now we have ISMRE. (This is news to me.)
I agree with Nick that it's not immediately apparent how one would convert full-load MRE to EER or part load ISMRE to IEER, for simulating the comparative energy performance of DX DOAS units.
Additionally:
* 1.) Should you model an ASHRAE Appendix G Baseline any differently if the Proposed Design uses a DX DOAS?
* 2.) What inputs are available in eQUEST to capture the energy savings or penalty?
1. 90.1-2013 added a requirement in Table G3.1(4.) that temperature and humidity setpoints and schedules and control throttling ranges be the same between proposed and baseline. If the use of a DX DOAS in the proposed design is part of an active control strategy or requirement to maintain a known maximum RH value in the zones, then you would also use that humidity setpoint in the baseline. However, use of a DX DOAS does not by itself correspond directly with any particular zone humidity level. I don't think there are circumstances that require modeling a DOAS in the baseline. Likewise, if the proposed design has no zone humidity controls, I don't think you would model the baseline with any.
2. DX DOAS per Standard 920 specifies a leaving-air dew point no higher than 55°F. This can be modeled in eQUEST/DOE-2.3 with the new SYSTEM:MAX-DEWPOINT keyword. Some other keywords that might need custom inputs include RATED-EDB, RATED-EWB, COIL-BF and COIL-BF-FT. If use of a DX DOAS in the proposed design is an effective proxy for zone humidity control, you could specify SYSTEM:MAX-HUMIDITY in the baseline system(s), and also in any proposed design systems served by a DOAS (but not the DOAS itself). The SS-N reports summarize the RH values in the system return air. You could use these values from the proposed design reports to inform values for baseline MAX-HUMIDITY.
Cheers,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
134 South Fitzhugh Street
Rochester, NY 14608 [cid:image004.png at 01D4EBBD.86DCCA70] Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Jones, Christopher via Equest-users
Sent: Friday, April 5, 2019 1:40 PM
To: Nicholas Caton <Nicholas.Caton at se.com>
Cc: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Modeling ISMRE
Hi Nick,
The tricky part is getting the performance data from the manufacturers. Back in the old days before the internet, the mechanical designer had huge binders from Trane, Carrier, etc. Those paper binders had much more performance data than available on line. You could pick up the performance of a unit at all those points in your table.
Christopher R Jones, P.Eng.
T+ 1 416-644-0252
[cid:image008.png at 01D4EBBD.86DCCA70]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Nicholas Caton via Equest-users
Sent: Friday, April 05, 2019 12:58 PM
To: Lee Shaver <lshaver at slipstreaminc.org<mailto:lshaver at slipstreaminc.org>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Modeling ISMRE
Fascinating! (I've got deadlines today so naturally something catches my eye in the mailing list...)
On first pass through that article, it seems to me that the ASHRAE 90.1 committee dropped the ball with respect to considering performance rating energy simulation inputs.
There appears to be no immediately clear path for an energy simulator to get from a prescribed minimum ISMRE / ISCOP to a steady state EER or COP inputs you could apply to typical/library performance curves.
It might be possible to iteratively worsen the inputs of a standard DX unit accomplishing dehumidification and hot gas reheat to generate 70F air, then calculate its resulting "virtual lab" ISMRE / ISCOP rating using custom hourly reports for capacity/input at the stated testing conditions from the new standard 920 (tables in the linked paper summarize)... tweaking the weather/loading profiles may be necessary to replicate each testing condition - not a small venture. You could alternatively assemble all of the associated library curves and make a virtual benchmarking spreadsheet to model in parallel what doe2 would output for power in and capacity given [evaporator DB, evaporator WB, condenser DB, PLR], which would make it easier to punch in the various PLR and temperature conditions as variables. You could then run a solver function on the steady state EIR you'll enter for the unit to arrive at the exact/target prescribed rating. You could then post here and potentially sell copies of your work for 5 bucks a pop until 90.1 catches up... I'd pay that readily if a conundrum like this were in front of me today.
[cid:image009.png at 01D4EBBD.86DCCA70]
Seems to me the ASHRAE Standard 90.1 committee has a little more homework to address this topic fully. I suggest either:
1. Come up with some concurrent steady-state performance criteria and a set of performance curves to fully describe the systems corresponding to the listed ISMRE / ISCOP ratings (rather than dump this legwork on all of the end-users, the majority of which will struggle and probably get the math wrong), or
2. Come up with a broad-stroke "derate" of the listed baseline efficiency for a normal DX system performing DOAS duties to fairly account for extra energies resulting from subcooling/hot gas reheat
Then again maybe I'm missing something... does this proposal make sense to anyone?
OK I better get back to work!
~Nick
[cid:image010.png at 01D4EBBD.86DCCA70]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Energy Performance Contracting
D
M
F
E
913 . 564 . 6361
785 . 410 . 3317
913 . 564 . 6380
nicholas.caton at se.com<mailto:nicholas.caton at se.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image011.png at 01D4EBBD.86DCCA70]
From: Equest-users <equest-users-bounces at lists.onebuilding.org<mailto:equest-users-bounces at lists.onebuilding.org>> On Behalf Of Lee Shaver via Equest-users
Sent: Friday, April 05, 2019 9:08 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Modeling ISMRE
[External email: Use caution with links and attachments]
________________________________
Hi all,
ASHRAE 90.1-2013 addendum cd adds tables 6.8.1-14 and -15 which include an ISMRE requirement for "electrically operated DX-DOAS units, single package and remote condenser."
ISMRE stands for "Integrated Seasonal Moisture Removal Efficiency" and is measured in pounds of water removed per kWh of electrical energy consumed (lb/kWh).
TRANE has a great article<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.trane.com%2Fcontent%2Fdam%2FTrane%2FCommercial%2Fglobal%2Fproducts-systems%2Feducation-training%2Fengineers-newsletters%2Fstandards-codes%2FADM-APN060-EN_110116.pdf&data=02%7C01%7CNicholas.Caton%40se.com%7Cb5c3aa2118f64e4f25fc08d6b9d0267e%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636900700993138894&sdata=hT9LSLOD1J9MJEZ%2F6wzWJ7tBS1Vzz4%2FdelUH9pTqhrE%3D&reserved=0> on ISMRE and why it's now included in ASHRAE 90.1.
Currently, I'm working on a model with a parametric run for a DOAS unit with an ISMRE that is better than baseline, and an EER that is worse than the baseline.
How can I accurately model this improvement in ISMRE, and the resulting reduction in energy usage for the DOAS units?
Googling "eQuest ISMRE" returns only four hits<https://eur02.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.google.com%2Fsearch%3Fq%3D%2522eQuest%2522%2B%2522ISMRE%2522&data=02%7C01%7CNicholas.Caton%40se.com%7Cb5c3aa2118f64e4f25fc08d6b9d0267e%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636900700993148902&sdata=hDJI4CoBE7wKIHzf2Y%2BvIVUjkVmwdyO22Dc8vkYuc%2FI%3D&reserved=0>, none of which are relevant.
Thanks,
Lee Shaver, Project Manager
Slipstream
608.210.7145 slipstreaminc.org<https://eur02.safelinks.protection.outlook.com/?url=http%3A%2F%2Fslipstreaminc.org%2F&data=02%7C01%7CNicholas.Caton%40se.com%7Cb5c3aa2118f64e4f25fc08d6b9d0267e%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636900700993148902&sdata=4%2B77LWmQyhiXmZPuASZ23n8oT1CXvmE4v5bE1d32F4g%3D&reserved=0>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190405/43eff8af/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190405/43eff8af/attachment-0006.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 1554 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190405/43eff8af/attachment-0015.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 1860 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190405/43eff8af/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 29435 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190405/43eff8af/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 255 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190405/43eff8af/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 8477 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190405/43eff8af/attachment-0019.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1903 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20190405/43eff8af/attachment-0007.jpg>
More information about the Equest-users
mailing list