[Equest-users] Exhaust Fan for Humidity Control
Nicholas Caton
Nicholas.Caton at schneider-electric.com
Fri Sep 14 09:56:11 PDT 2018
Hi Paul,
To my knowledge, there’s no explicit option in equest for tying a fan/process energy to an interior/exterior humidity state. Some pre-processing/work outside your model would be necessary.
You could do an analysis separately in excel (ideally informed with field measurements of an existing/built situation) with intent to ultimately estimate fan runtime, and then “spoon feed” the outcome of your efforts into an eQuest model in the form of a fan schedule and some power inputs at the meter. The likes of EMIT can make the transition from spreadsheet efforts easier.
I might however first want to take a step back and draw caution towards understanding more of the context behind this measure… I’m reminded that Mr. Lstiburek’s articles in the ASHRAE journals and beyond (hosted here: https://buildingscience.com/document-search <-- you can filter results by ticking the box for “Crawlspaces”) repeatedly warn against passively/actively ventilating building crawlspaces to/from the exterior. It’s my general sense that active ventilation with exterior conditions can generally cause more problems than it solves with regard to humidity/moisture issues. If however we’re talking about circulation of conditioned (interior) air and treating the crawlspace like a conditioned/sealed basement, that’s approaching an “ideal” state WRT moisture control.
I hope this is a little helpful!
~Nick
[cid:image001.png at 01D44C19.6DAEC290]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D44C19.6DAEC290]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of Paul Diglio via Equest-users
Sent: Tuesday, September 11, 2018 8:07 AM
To: equest-users at onebuilding.org
Subject: [Equest-users] Exhaust Fan for Humidity Control
Hi All:
Is there anyway to model an exhaust fan that only runs when the humidity in a crawl space is above a certain setpoint?
Thank you,
Paul Diglio
87 Fairmont Avenue
New Haven, CT 06513
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/4aeaabfa/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/4aeaabfa/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/4aeaabfa/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7119 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/4aeaabfa/attachment.obj>
More information about the Equest-users
mailing list