[Equest-users] Building Rotation
Nicholas Caton
Nicholas.Caton at schneider-electric.com
Fri Sep 14 08:35:35 PDT 2018
Hi John,
There isn’t a 1-click step for building rotations, but it’s relatively simple with a framework like this. You want to use parametric runs to adjust the AZIMUTH property for each of your floors. If from wizards development you haven’t messed with or provided manual rotation inputs to any of the shell/space/geometry defaults for azimuth, everything should rotate together based on this input alone:
[cid:image007.png at 01D44C16.A8C0B4E0]
The above illustrates how I’d prefer to document/structure a building where “Plan North” starts at 110 degrees from true North, as you prompted. Note the final input for AZIMUTH will throw an error if the value is either >360 or <-360, so if your baseline is 110 we can’t add 270 for the final rotation but must instead turn the other direction (-90)…
Does this answer the question?
~Nick
[cid:image001.png at 01D44C15.A8132C40]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image002.png at 01D44C15.A8132C40]
From: Equest-users <equest-users-bounces at lists.onebuilding.org> On Behalf Of John Aulbach via Equest-users
Sent: Tuesday, September 11, 2018 7:30 PM
To: equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Green power
[External email: Use caution with links and attachments]
________________________________
Building Rotation:
It is easy if your original building faces 0 Deg North, and you do 90 Deg rotations for orientation, But what if your North is, say, 110 DegE. Is there a simple parametric to make the facing directions correct? Or must I put in the actual compass directions?
John
On Tuesday, September 11, 2018, 1:17:41 PM PDT, Bishop, Bill via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
Hi Tejas,
Try this EPA document<https://emea01.safelinks.protection.outlook.com/?url=https%3A%2F%2Fwww.epa.gov%2Fsites%2Fproduction%2Ffiles%2F2016-01%2Fdocuments%2Fpurchasing_guide_for_web.pdf&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7Ce87bcb5e244549fad71e08d61846f852%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636723090423182492&sdata=4jWQXDoKqaU8IIXx2EEyIhj9FnD1SEa1zuwnM6%2BNNFw%3D&reserved=0>, newly updated, for explanations of the variations of “Green Power”.
My attempt at an explanation: Green power and RECs are products that capture the benefit of renewable electricity generation at an off-site location.
You can think of RECs as the added value of renewable electricity versus fossil-fuel generated electricity. Solar power is awesome! Coal-fired power is still pretty impressive. If you want to pay for the difference between awesome and impressive, you buy RECs.
What if you want to buy all the awesome, including the electricity itself? You buy Green power/energy. You purchase green power through an electric utility (or an energy supplier, depending on how the electricity market is regulated where you live). You pay for the same electricity that was going to come in through your electric service no matter who you bought it from or how much you paid for it. But you also pay for the added value of an equivalent amount of renewable energy that was generated somewhere else. Buying green power is basically buying dirty power + RECs.
Note: “Green power” is not the same as “on-site renewables”. Installing solar PV or wind power etc. on the building or building site is covered in LEED V4 “Renewable Energy Production”.
I have a cynical view of carbon offsets and will just leave it at that.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.pathfinder-ea.com%2F&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7Ce87bcb5e244549fad71e08d61846f852%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636723090423182492&sdata=pw7ieWLa0T%2FgSCcx%2B1pDIfDDALWX3vKeht5K258ph4E%3D&reserved=0>
[cid:image009.png at 01D44C16.A8C0B4E0]134 South Fitzhugh Street
Rochester, NY 14608 Ask me why Carbon Fee & Dividend may be right for you.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Dante Garcia via Equest-users
Sent: Tuesday, September 11, 2018 10:49 AM
To: equest user <equestuser00 at gmail.com<mailto:equestuser00 at gmail.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Green power
Hi.
Carbon offsets mitigate the carbon dioxide produced due to source energy consumption in your building. For instance, if your building generate 1 Ton CO2, a carbon offset of 1 Ton CO2 indicates that your CO2 generated is absorved anywhere in the world. You buy this certificate.
RECs are certificates that electricity is generated by a renewable sources. For instance, if your site building consumption is 1 MWh, a REC of 1 (MWh) indicates that the energy your building use is also generated by renewable sources anywhere in the world. You buy this certificate. For LEED RECs should be Green-e certified or equivalent.
Green Power is renewable energy produced on-site and also used in your building.
Hope that helps,
On Tue, Sep 11, 2018 at 3:20 AM, equest user via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:
Hi all eQUEST users,
Can anyone enlighten me on what is the exact difference between Carbon offsets, REC and green power.
This query is regarding the LEED V4 rating system credit: green power and carbon offsets.
I am kinda confused with this, would really appreciate if someone helps!!!
Thanks,
Tejas
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7Ce87bcb5e244549fad71e08d61846f852%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636723090423182492&sdata=bZSacp7dnXRdJdzFZMAI3979d%2FX0sPTn5L16hkbkrVc%3D&reserved=0>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
--
SUMAC
Dante Garcia // LEED AP BD+C
Analista LEED Energía
Tel: + 511 253.5355 Anexo 10(Lima, Perú)
dgarcia at sumacinc.com<mailto:dgarcia at sumacinc.com>
www.sumacinc.com<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Fwww.sumacinc.com%2F&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7Ce87bcb5e244549fad71e08d61846f852%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636723090423182492&sdata=Ba%2FZmGPDORD4D3bCpRKzwpx8z58ow1hCV5JBT0rP9bs%3D&reserved=0>
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org<https://emea01.safelinks.protection.outlook.com/?url=http%3A%2F%2Flists.onebuilding.org%2Flistinfo.cgi%2Fequest-users-onebuilding.org&data=02%7C01%7Cnicholas.caton%40schneider-electric.com%7Ce87bcb5e244549fad71e08d61846f852%7C6e51e1adc54b4b39b5980ffe9ae68fef%7C0%7C0%7C636723090423182492&sdata=bZSacp7dnXRdJdzFZMAI3979d%2FX0sPTn5L16hkbkrVc%3D&reserved=0>
To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/317e4990/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 255 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/317e4990/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 8477 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/317e4990/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 2256 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/317e4990/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: oledata.mso
Type: application/octet-stream
Size: 7146 bytes
Desc: oledata.mso
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/317e4990/attachment.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 55833 bytes
Desc: image007.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/317e4990/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.jpg
Type: image/jpeg
Size: 1813 bytes
Desc: image008.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/317e4990/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 1531 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180914/317e4990/attachment-0003.png>
More information about the Equest-users
mailing list