[Equest-users] Baseline has space heat, but proposed has zero space heat

Daric Adair Daric.Adair at hendersonengineers.com
Tue Nov 13 13:56:35 PST 2018


Jing;

Some ideas:
1-see other email on System Heating Temperatures.
2-The Capacities are based on the Heating & Cooling Degree (HDD/CDD) days (if entered) or from the weather file if no HDD/CDD is specified (I believe). The System Sizing, Cooling Sizing Ratio, and Heating Sizing Ratio are all used, if entered. They default to 1.0 if no capacities are entered, or grey out if capacities are entered.  The sizing calculations are the first ~20% of the eQuest simulation. On SV-A the Heating and Cooling Capacities will be shown at the top. The Zone Heating Capacities should show up on a zone by zone basis in the table below. Right now shown as ‘0.0’, most likely due to issue(s) from other email.
3-These can be confusing. The Cooling Capacity is a function of if there is a zoing cooling coil (theres not in a VAV system) The Extraction Rate is the calculation to determine what the maximum heat which can be extracted from the zone, based on the airflow and temperature difference of the Design-Cool-T and the Min-Supply-T. The Heating Capacity is the capacity of the zone heating coil (reheat coil in a VAV case) and is the 1.08*CFM*Reheat_deltaT*Supply Ratio. The Addition Rate is similar, though it is 1.08*CFM*(Max-Supply-T  -  Design Heat-T)*Supply Ratio.




Thanks,
DARIC R ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst

Henderson Engineers
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>

Licensed in KS

From: Jing Hong <hongjing.shirley at gmail.com>
Sent: Monday, November 12, 2018 4:59 PM
To: equest-users at lists.onebuilding.org; equest-users at onebuilding.org
Subject: [Equest-users] Baseline has space heat, but proposed has zero space heat

Dear All,

I have a model located in Mexico. The baseline is equipped with PSZ+Heat pump and proposed is equipped with VFD + Heat pump. For some reasons, the baseline has a normal space heat, but the proposed shows 0 space heat. The envelop, schedule, setpoints, outside air flow rates are all the same.
1. What could be the possible reason for something like this?
2. Does anyone know how eQuest calculate the heating/cooling capacity at the system and zone level? For example, I set up the cooling and heating capacity for the system and set up setpoints for each zone. So in the SV-A, it only shows the heating/cooling capacity of the system, and for each zone will be zero heating and cooling capacity?
3. What is the extraction rate (KBTU/HR) and addition rate(KBTU/HR) in SV-A? Where are they from?

[image.png]

[image.png]

Thank you!

________________________________

This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/235c0d82/attachment-0003.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 46611 bytes
Desc: image002.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/235c0d82/attachment-0014.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 47305 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181113/235c0d82/attachment-0015.png>


More information about the Equest-users mailing list