I don’t think there is any way to reference U-NAMEs in expressions.
An alternative is to create the Global parameters by system number (in order that the systems are created), not by system name.
For example:
Your model has 10 systems. The first four systems that you define are packaged VAV systems named, in order of creation, “1stFlrN-PVAV”, “1stFlrS-PVAV”, “2ndFlrN-PVAV”, “2ndFlrS-PVAV”.
You want to assign unique COOLING-EIR to each system. You could use the following BDL input:
PARAMETER
"1st-system-CLG-EIR" = 0.310 ..
PARAMETER
"2nd-system-CLG-EIR" = 0.320 ..
PARAMETER
"3rd-system-CLG-EIR" = 0.330 ..
PARAMETER
"4th-system-CLG-EIR" = 0.340 ..
SET-DEFAULT FOR SYSTEM
TYPE = PVAVS
COOLING-EIR =
{switch #SV(#LS())
case 1 : #PA("1st-system-CLG-EIR") $ 1stFlrN-PVAV
case 2 : #PA("2nd-system-CLG-EIR") $ 1stFlrS-PVAV
case 3 : #PA("3rd-system-CLG-EIR") $ 2ndFlrN-PVAV
case 4 : #PA("4th-system-CLG-EIR") $ 2ndFlrS-PVAV
default : 0.360
endswitch}
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer
[cid:image005.jpg at 01D3BF93.52A921B0] [cid:image007.jpg at 01D3BF93.52A921B0]
134 South Fitzhugh Street Rochester, NY 14608
T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher via Equest-users
Sent: Monday, March 19, 2018 2:05 PM
To: Nicholas Caton <Nicholas.Caton at schneider-electric.com>
Cc: equest-users at onebuilding.org
Subject: Re: [Equest-users] Another Keyword Expression question
Nick, Bill
I miss phrased the question. The expression should retrieve the system name, “SysName”, concatenate “-CLG-EIR” the set COOLING-EIR to “SysName-CLG-EIR” which is a parameter defined in Global parameters.
So the keyword expression would be in the COOLING-EIR Edit/View User Expression entry.
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image010.png at 01D3BF8E.8AEEE690]
T +1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
From: Nicholas Caton [mailto:Nicholas.Caton at schneider-electric.com]
Sent: Monday, March 19, 2018 1:41 PM
To: Jones, Christopher <Christopher.r.Jones at wsp.com<mailto:Christopher.r.Jones at wsp.com>>
Cc: equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Subject: RE: Another Keyword Expression question
Request unclear… is this right?
1. You want an expression for a ZONE input to vary based on the string which is the name of the parent SYSTEM?
2. You further want a global parameter (#PA) defined as a string to be returned for insertion into said expression?
Maybe another line of context as to what you’re trying to achieve could help as well =).
~Nick
[cid:image011.png at 01D3BF8E.8AEEE690]
Nick Caton, P.E., BEMP
Senior Energy Engineer
Regional Energy Engineering Manager
Energy and Sustainability Services
Schneider Electric
D 913.564.6361
M 785.410.3317
F 913.564.6380
E nicholas.caton at schneider-electric.com<mailto:nicholas.caton at schneider-electric.com>
15200 Santa Fe Trail Drive
Suite 204
Lenexa, KS 66219
United States
[cid:image012.png at 01D3BF8E.8AEEE690]
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Jones, Christopher via Equest-users
Sent: Monday, March 19, 2018 12:07 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] Another Keyword Expression question
I am looking for a way to retrieve the SYSTEM NAME from a child of system. For example:
COOLING-EIR = (#PA(“SysName-CLG-EIR”)
Where SysName-CLG-EIR is a parameter like “Parking Garage System-COP-EIR”
Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy
[cid:image001.png at 01D3BF81.1A482B20]
T +1 416-644-0252
2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com
Please consider the environment before printing...
________________________________
NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.
AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.
-LAEmHhHzdJzBlTWfa4Hgs7pbKl
______________________________________________________________________
This email has been scanned by the Symantec Email Security.cloud service.
______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180319/5305863e/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 25844 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180319/5305863e/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 255 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180319/5305863e/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image012.png
Type: image/png
Size: 8477 bytes
Desc: image012.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180319/5305863e/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: image005.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180319/5305863e/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: image007.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180319/5305863e/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image009.png
Type: image/png
Size: 3859 bytes
Desc: image009.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180319/5305863e/attachment-0003.png>
More information about the Equest-users
mailing list