[Equest-users] Loop to Loop Heat Pump Error

PKConsulting pasha.pkconsulting at gmail.com
Fri Mar 16 16:53:40 PDT 2018


Hi Anthony,  yes I can.  I hope to finish this model this weekend.

Pasha
Ph: 308-763-1593

> On Mar 8, 2018, at 10:32 AM, Anthony <Anthony at GreenEngineer.com> wrote:
> 
> Pasha, would you mind sharing the “working” inp/pd2 when you’re done?  I’ll be facing the same issue shortly.
>  
> Anthony Hardman, PE, BEAP, LEED AP BD+C
> Senior Building Performance Analyst
> The Green Engineer, Inc.
> (978) 610-2801
>  
> From: Pasha Korber-Gonzalez [mailto:pasha.pkconsulting at gmail.com] 
> Sent: Wednesday, March 7, 2018 5:05 PM
> To: Nicholas Caton
> Cc: Bishop, Bill; equest-users at onebuilding.org; David Eldridge
> Subject: Re: [Equest-users] Loop to Loop Heat Pump Error
>  
> Hello & THANK YOU to Bill, Nick, David, Brian, & Jeff!
>  
> I always appreciate you all taking time out of your busy busy schedules to offer some help.   I am just now able to get back to my computer and work on the project tonight.  I will re-look at my file and try the suggestions you all have made.   Fingers-crossed it all goes smooth for this attempt.
>  
> Cheers,
> Pasha
>  
> Ph: 308-763-1593
>  
> On Wed, Mar 7, 2018 at 2:27 PM, Nicholas Caton <Nicholas.Caton at schneider-electric.com> wrote:
> Sorry for omitting some of these helpful details.
>  
> I too am loading and running in DOE2.2 mode from build 7174
> I can’t be completely certain as I didn’t keep good records of my install files, but I believe this is build currently published in the doe2.com downloads section, tagged “release testing” (or similar)
> Commenting to Bill’s suggestion, as I loaded this up I did look for and find those four values are defaulted, but they don’t appear to line up with the values listed in your original error for Ti (in) and To (out) for the two sides of the HX.  You might additionally try manually setting these inputs to match mine regardless of how they default in your instance:
> <image001.png>
> 
>  
> <image002.png>
> Nick Caton, P.E., BEMP
>   Senior Energy Engineer
>   Regional Energy Engineering Manager
>   Energy and Sustainability Services
>   Schneider Electric
> D  913.564.6361 
> M  785.410.3317 
> F  913.564.6380
> E  nicholas.caton at schneider-electric.com
> 15200 Santa Fe Trail Drive
> Suite 204
> Lenexa, KS 66219
> United States
> <image003.png>
>  
>  
> From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com] 
> Sent: Wednesday, March 07, 2018 8:23 AM
> To: PKConsulting <pasha.pkconsulting at gmail.com>
> Cc: equest-users at onebuilding.org; David Eldridge <DEldridge at grummanbutkus.com>; Nicholas Caton <Nicholas.Caton at schneider-electric.com>
> Subject: RE: [Equest-users] Loop to Loop Heat Pump Error
>  
> Pasha,
> Like Nick, I had no problem getting the model to run using 3.65 build 7174 in DOE2.2 mode.
> It also runs in 3.64 build 7130, once I remove the line “HVACDefaulted = 1” from the pd2 file.
> A couple suggestions:
> Go to the Miscellaneous tab of the chiller and Restore Default to the four Heat Exchanger inputs. The error message you sent makes me think these have non-default values.
> Copy the .pd2 and .inp files you sent into a new folder and try opening it again.
> Regards,
> ~Bill
>  
> William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
> Senior Energy Engineer
> <image004.jpg>  <image005.jpg>
>  
> 134 South Fitzhugh Street                 Rochester, NY 14608
> T: (585) 698-1956                        F: (585) 325-6005
> bbishop at pathfinder-ea.com             www.pathfinder-ea.com
> <image006.png>Carbon Fee and Dividend - simple, effective, and market-based.
>  
> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of David Eldridge via Equest-users
> Sent: Tuesday, March 06, 2018 10:34 PM
> To: PKConsulting <pasha.pkconsulting at gmail.com>; Nicholas Caton <Nicholas.Caton at schneider-electric.com>
> Cc: equest-users at onebuilding.org
> Subject: Re: [Equest-users] Loop to Loop Heat Pump Error
>  
> Hopefully Nick’s software version control works. If not, maybe you can track down those keywords in the BDL(?) file – I forget – the file with the compiled syntax, where the INP doesn’t echo back fields with default values?
>  
> David
>                                                                                                
>  
> David S. Eldridge, Jr., P.E., LEED AP BD+C, BEMP, BEAP, HBDP
> Grumman/Butkus Associates
>                                                                                                
>  
>  
> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of PKConsulting via Equest-users
> Sent: Tuesday, March 06, 2018 6:53 PM
> To: Nicholas Caton <Nicholas.Caton at schneider-electric.com>
> Cc: equest-users at onebuilding.org
> Subject: Re: [Equest-users] Loop to Loop Heat Pump Error
>  
> Thanks David,  at this point I just don’t know.  I looked through the .inp file too and couldn’t find those keywords either.  That is when I turned to the group for more help.
> I’m completely stumped on this one...
> 
> Pasha
> Ph: 308-763-1593
> 
> On Mar 6, 2018, at 4:10 PM, Nicholas Caton <Nicholas.Caton at schneider-electric.com> wrote:
> 
> Would it bug you to learn this loads and simulates without error on my end?
>  
> Gut check:  are you being deliberate to open and simulate with the “release testing” build 7174?
>  
> ~Nick
>  
> <image001.png>
> Nick Caton, P.E., BEMP
>   Senior Energy Engineer
>   Regional Energy Engineering Manager
>   Energy and Sustainability Services
>   Schneider Electric
> D  913.564.6361 
> M  785.410.3317 
> F  913.564.6380
> E  nicholas.caton at schneider-electric.com
> 15200 Santa Fe Trail Drive
> Suite 204
> Lenexa, KS 66219
> United States
> <image002.png>
>  
>  
> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez via Equest-users
> Sent: Tuesday, March 06, 2018 3:11 PM
> To: eQUEST Users List <equest-users at lists.onebuilding.org>
> Subject: [Equest-users] Loop to Loop Heat Pump Error
>  
> Hi All,
>  
> does anyone have any experience with modeling the Loop to Loop Heat Pump chiller?  I'm getting the following error in my file, and right now I am auto-sizing everything just to test it to get the file to run.  I cannot locate/find where the Qhx Design, SupFlow, SupTi, SupTo key words are linked too.  The heat-Exchanger: HRC-T1 is the name of my LtLHP Chiller that I input on the loops.
>  
> I've looked through the DOE-2 documents for LtLHP chiller and I can't find where this error is occurring so that I can fix it.  Any insight you can offer will be appreciated.  
>  
> I've also attached my .pd2 & .inp files if anyone is inclined to look at them.  Thanks in advance for sharing your thoughts and your brains with me!
>  
>  
>  ***ERROR***********************************************************************
>              Heat-Exchanger: HRC-T1                           has
>              inconsistent design parameters:
>               QhxDesign   SupFlow     SupTi     SupTo
>                3541040.      708.      85.0      95.0
>                           DemFlow     DemTi     DemTo
>                              708.      85.0      75.0
>  
>  
> Pasha
> Ph: 308-763-1593
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
> 
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.