 My best guess (assuming you want cooling for example) is to make a single chiller for your building (gotta be PLANT equipment). Figure out the peak cooling load from SS-D and size the chiller accordingly. Run the building. Look in PS-C, with 10% increments of load.
Multiply each 10% load increment (say chiller is 1000 ton, so 100 tons for 10%, 200 tons for 20%, etc) by the number of hours shown for that increment. Take the total ton-hrs and divide by the 1000 ton (for this example).
That should give you equivalent load hours.
John Aulbach, PE
    On Wednesday, March 14, 2018, 2:27:48 PM PDT, Daric Adair via Equest-users <equest-users at lists.onebuilding.org> wrote:  
 
  <!--#yiv1848449785 _filtered #yiv1848449785 {font-family:"Cambria Math";panose-1:2 4 5 3 5 4 6 3 2 4;} _filtered #yiv1848449785 {font-family:Calibri;panose-1:2 15 5 2 2 2 4 3 2 4;}#yiv1848449785 #yiv1848449785 p.yiv1848449785MsoNormal, #yiv1848449785 li.yiv1848449785MsoNormal, #yiv1848449785 div.yiv1848449785MsoNormal {margin:0in;margin-bottom:.0001pt;font-size:11.0pt;font-family:"Calibri", sans-serif;}#yiv1848449785 a:link, #yiv1848449785 span.yiv1848449785MsoHyperlink {color:#0563C1;text-decoration:underline;}#yiv1848449785 a:visited, #yiv1848449785 span.yiv1848449785MsoHyperlinkFollowed {color:#954F72;text-decoration:underline;}#yiv1848449785 span.yiv1848449785EmailStyle17 {font-family:"Calibri", sans-serif;color:windowtext;}#yiv1848449785 .yiv1848449785MsoChpDefault {font-family:"Calibri", sans-serif;} _filtered #yiv1848449785 {margin:1.0in 1.0in 1.0in 1.0in;}#yiv1848449785 div.yiv1848449785WordSection1 {}-->
Does anyone know if there is a report or means from eQuest to generate the EFLH (equivalent full load hours) for each schedule?
 
Colleague of mine believes VistualDOE was able to complete and hoping there is a comparable tool/report.
 
  
 
Thanks in advance.
 
  
 
  
 
  
 
Thanks,
 
DARIC R ADAIR PE, CEM, BEMP 
Mechanical Engineer, Energy Analyst 

Henderson Engineers
8345 Lenexa Drive, Suite 300  |  Lenexa, KS 66214
Tel (913) 742-5530  
daric.adair at hendersonengineers.com

hendersonengineers.com

Licensed in KS

Sending me large files? Please useHenderson File Share | TX ID #F-001236
 
  
 

This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com.
_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
  
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180315/64d49673/attachment.html>


More information about the Equest-users mailing list