Bill,
The great majority of high rise multi-family buildings are condominiums (like your co-ops). Each suite is metered for electricity directly by the utility so the designs try to get as much electricity into the suites. Then there is the all glazing fad that isn’t fading. In order to meet the local code, you need condensing boilers for heating and air side heat recovery therefore the insuite ERVs.

Note, all designs also include a makeup air system for corridor pressurization (mostly for odor control) and there is no return to these make-up air systems. 50 cfm per suite is the typical amount dumped into the corridors. As well, most of these buildings pursue LEED therefore have weather stripping on the suite doors for the tobacco prerequisite. I don’t know where all that corridor pressurization makeup air goes.




Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy

[cid:image001.png at 01D3B77C.80DD70A0]
T +1 416-644-0252

2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada

wsp.com


Please consider the environment before printing...


From: Bishop, Bill [mailto:bbishop at pathfinder-ea.com]
Sent: Thursday, March 08, 2018 2:06 PM
To: Jones, Christopher <Christopher.r.Jones at wsp.com>
Subject: RE: [Equest-users] exhaust heat recovery system with PTAC in eQUEST

Does your local code require ERVs for each suite?

From: Jones, Christopher [mailto:Christopher.r.Jones at wsp.com]
Sent: Thursday, March 08, 2018 1:22 PM
To: Bishop, Bill <bbishop at pathfinder-ea.com<mailto:bbishop at pathfinder-ea.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: RE: [Equest-users] exhaust heat recovery system with PTAC in eQUEST

Hi Bill,
We have been around that exception a number of times. The conclusion reached is that exception 8 does not apply if each suite has an ERV responsible for the outdoor air and exhaust of that suite.

If the building has a central make-up air system dumping air into the corridors, through the carpet filter under the doors into the suites, then locally exhausted, then exception 8 does apply.

Here in Ontario we model the baseline as per Section 11, ECB. Most new apartment buildings have insuite ERVs and fan coils. Therefore the baseline suite systems also have heat recovery.


Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy

[cid:image001.png at 01D3B77C.80DD70A0]
T +1 416-644-0252

2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com


Please consider the environment before printing...


From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Bishop, Bill via Equest-users
Sent: Thursday, March 08, 2018 1:00 PM
To: sunayana jain <sunayanajn at gmail.com<mailto:sunayanajn at gmail.com>>
Cc: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] exhaust heat recovery system with PTAC in eQUEST

Hi Sunayana,
Use Pkgd Single Zone (PSZ) systems to model Appendix G PTACs. You will need to create one PSZ system per zone which might mean 100+ systems for your 6-story apartment building. Floor multipliers are probably in order.
The PTAC fan power of 0.0003 kW/cfm includes ERVs. I’m not aware of an exception to Appendix G that would apply.
There are a few possibilities for justifying no ERV in the baseline:

  *   Ventilation system runs <8000 hrs/year (hard to justify for apartments?)
  *   The building is a multipurpose use and you can model additional system types in the nonresidential areas
  *   6.5.6.1 exception (8.), “where the largest source of air exhausted at a single location at the building exterior is less than 75% of the design outdoor airflow rate”. This would seem to apply, since each PTAC handles the ventilation load for one zone, and the baseline would have no large common exhaust location.
Regards,
~Bill

William Bishop, PE, BEMP, BEAP, CEM, LEED AP | Pathfinder Engineers & Architects LLP
Senior Energy Engineer

[cid:image002.jpg at 01D3B77C.80DD70A0]  [cid:image003.jpg at 01D3B77C.80DD70A0]



134 South Fitzhugh Street                 Rochester, NY 14608

T: (585) 698-1956                        F: (585) 325-6005

bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com>             www.pathfinder-ea.com<http://www.pathfinder-ea.com/>

[http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon Fee and Dividend - simple, effective, and market-based.


From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of sunayana jain via Equest-users
Sent: Thursday, March 08, 2018 11:16 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: [Equest-users] exhaust heat recovery system with PTAC in eQUEST

As per ASHRAE 90.1-2013, exhaust air energy recovery is required for ventilation systems operating greater than 8000 hours per year. I am working on a baseline model of 6 storeys apartment building in climate zone 5A. As per ASHRAE 90.1-2013 Appendix G, apartments units are required to have PTAC systems with heat recovery. I am wondering, how to model PTAC with heat recovery in eQUEST. PTAC system cannot take heat recovery in eQUEST.
Also, ASHRAE does not have any information on fan power for energy recovery systems. Should the ERV fan be a part of allowable 0.0003 kW/cfm fan power?
Any suggestions will be appreciated.
Thanks,
Sunayana Jain


________________________________


NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.

AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.



-LAEmHhHzdJzBlTWfa4Hgs7pbKl
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180309/f505bc4a/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180309/f505bc4a/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 1240 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180309/f505bc4a/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1311 bytes
Desc: image003.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180309/f505bc4a/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 2851 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180309/f505bc4a/attachment-0001.png>


More information about the Equest-users mailing list