[Equest-users] Loop to Loop Heat Pump Error
PKConsulting
pasha.pkconsulting at gmail.com
Tue Mar 6 16:51:16 PST 2018
Hi Nick- yes I am using the 7174 build. And I even tried Doe 2-3, which doesn’t support geothermal loops and LtLHP chillers.
Are you using the previous build version? If yes, then I will go back to that for this model...
Thanks!
Pasha
Ph: 308-763-1593
> On Mar 6, 2018, at 4:10 PM, Nicholas Caton <Nicholas.Caton at schneider-electric.com> wrote:
>
> Would it bug you to learn this loads and simulates without error on my end?
>
> Gut check: are you being deliberate to open and simulate with the “release testing” build 7174?
>
> ~Nick
>
> <image001.png>
> Nick Caton, P.E., BEMP
> Senior Energy Engineer
> Regional Energy Engineering Manager
> Energy and Sustainability Services
> Schneider Electric
> D 913.564.6361
> M 785.410.3317
> F 913.564.6380
> E nicholas.caton at schneider-electric.com
> 15200 Santa Fe Trail Drive
> Suite 204
> Lenexa, KS 66219
> United States
> <image002.png>
>
>
> From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Pasha Korber-Gonzalez via Equest-users
> Sent: Tuesday, March 06, 2018 3:11 PM
> To: eQUEST Users List <equest-users at lists.onebuilding.org>
> Subject: [Equest-users] Loop to Loop Heat Pump Error
>
> Hi All,
>
> does anyone have any experience with modeling the Loop to Loop Heat Pump chiller? I'm getting the following error in my file, and right now I am auto-sizing everything just to test it to get the file to run. I cannot locate/find where the Qhx Design, SupFlow, SupTi, SupTo key words are linked too. The heat-Exchanger: HRC-T1 is the name of my LtLHP Chiller that I input on the loops.
>
> I've looked through the DOE-2 documents for LtLHP chiller and I can't find where this error is occurring so that I can fix it. Any insight you can offer will be appreciated.
>
> I've also attached my .pd2 & .inp files if anyone is inclined to look at them. Thanks in advance for sharing your thoughts and your brains with me!
>
>
> ***ERROR***********************************************************************
> Heat-Exchanger: HRC-T1 has
> inconsistent design parameters:
> QhxDesign SupFlow SupTi SupTo
> 3541040. 708. 85.0 95.0
> DemFlow DemTi DemTo
> 708. 85.0 75.0
>
>
> Pasha
> Ph: 308-763-1593
>
> ______________________________________________________________________
> This email has been scanned by the Symantec Email Security.cloud service.
> ______________________________________________________________________
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180306/6a285ed4/attachment-0002.htm>
More information about the Equest-users
mailing list