[Equest-users] Infiltration issues whith more than one shell

Daric Adair Daric.Adair at hendersonengineers.com
Fri Mar 2 13:59:51 PST 2018


-eQuest Digest just came thru – receiving emails out of order. Sorry in advance.

The infiltration rates from the example are from the eQuest Wizard input. The wizard input is expressed in a CFM/SF of exterior wall area. When the model is generated out of wizard and into the detailed/spreadsheet interface these infiltration rates are calculated/converted based on:

SpaceInfiltration [CFM/sf-floor] = (infiltration rate [CFM/sf-exterior wall area] * exterior wall area [sf]) / (Space Area [sf-space])
Note: INF-METHOD= AIR-CHANGE for this conversion/calculation.

I checked these for the example I sent out, and they aligned with the screenshots.

Joe - you are entirely correct that once in eQuest detailed edit mode, the Infiltration is expressed normalized to Space Area. Once past Wizard it is not possible to directly enter an infiltration in (CFM/sf-ExteriorWall area) without either doing some math outside of eQuest to normailze to the Space Area or using a UserExpression to do the same. (and very time consuming too. Learned the hard way -once).
The ‘EFFECTIVE-LEAKAGE-FRACTION’ input you reference is part of the Sherman-Grimsrud method; yes? The screen shots of the infiltration rates are of the ‘INF-FLOW/AREA’ input, which is default out of eQuest I believe.  This may be part of the confusion. Again, getting emails out of order.

Is there a report which contains a ‘whole building infiltration CFM’? I can find ACH by space, but nothing for the total building.

PNNL, NIST, and ASHRAE Journal have put out several reports in the last few years on the topic of energy models and infiltration. They use SF of exterior envelope  (not just wall or roof) as a metric in several reports. ASHRAE 90.1-2013 Appendix G now has requirements on how Infiltration must be included in an energy model. One of the reports “…recommends a rate of 1.8 CFM/sf (0.3 inwc) of exterior above grade envelope surface area.” (whoa, that’s higher than I’m used to seeing!)


To go back to the original question from Menush. The issue was two shells touching and that exterior walls are created for each shell, not an interior wall between the two shells (& respective zones. The question (as I understand it) has nothing to do with the realities of infiltration or methods there-of. The issue was that eQuest Wizard does not know that when two horizontal shells are touching that this is most likely an interior wall between spaces. And thus it creates ‘extra’ exterior walls which inflate the infiltration rate. This is accurate and the only point I was initially addressing (and I think Bruce was addressing similarly).  The methods on how to determine a proper infiltration rate for the impacted Spaces has sprung from this original question.

Menush – does this answer your question(s) on the shell/space/exterior walls coming out of wizard?




Thanks,
DARIC R ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst

Henderson Engineers
Tel (913) 742-5530
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>

Licensed in KS

From: Joe Huang [mailto:yjhuang at whiteboxtechnologies.com]
Sent: Friday, March 2, 2018 2:40 PM
To: Daric Adair <Daric.Adair at hendersonengineers.com>; Bruce Easterbrook <bruce5 at bellnet.ca>; equest-users at lists.onebuilding.org
Subject: Re: [Equest-users] Infiltration issues whith more than one shell


The point I'm trying to make is that DOE-2 and presumably eQUEST derives the infiltration rate from user input of the EFFECTIVE-LEAKAGE-FRACTION for the SPACE that is expressed in CFM/ft2 of floor area. This infiltration rate is not affected by the amount of exterior walls in the spaces or their proximity to each other.  In your examples, aren't the infiltration rates for the building just the sum of the infiltration rates for the zones (presumably perimeter and core) adjusted by their floor area ?

Joe

Joe Huang

White Box Technologies, Inc.

346 Rheem Blvd., Suite 205A

Moraga CA 94556

yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>

http://weather.whiteboxtechnologies.com for simulation-ready weather data

(o) (925)388-0265

(c) (510)928-2683

"building energy simulations at your fingertips"
On 3/2/2018 7:33 AM, Daric Adair wrote:
All;
Confused as to how Bruce’s answer isn’t directly applicable. What he detailed in the first instance is directly in line with my experiences. eQuest wizard modes doesn’t realize that two abutting/touching shells should have interior walls. If a space wall touches a shell wall, an exterior wall is created.

-          If a zone boarders a shell, eQuest creates an exterior wall.

-          If a zone does not touch a shell edge, eQuest makes an adiabatic interior wall.

-          If two shells are touching and each have zones touching the common wall, two exterior walls are created; one in each zone. Wizard eQuest doesn’t distinguish if two shells are 0 feet apart/touching or if they are 25 feet apart.  (example described below)
If eQuest uses exterior wall area to calculate a floor area normalized infiltration rate, and there are ‘extra’ exterior walls which are actually interior walls where shells touch, then the infiltration rate will be  calculated as though the two shells were never touching. This will increase the calculated infiltration rate since these are not actually interior walls.

Bruce’s solution only neglected to mention that the infiltration rate will either need to be corrected for this condition, or ignored/neglected. The second option is not to say infiltration is not important – it is important – but requires modeler judgement and some math. The length/area of the touching walls is also a factor to consider. If project is a large industrial setting as described in thread, yes, probably should check/revise. If a small connecting corridor, probably minor and can be ignored.


Did a quick (very simplified ) example. All examples have: 10ft high. No plenum. Set Perimeter infiltration to 0.05 CFM/sf. 0.0 core infiltration.
- Made two shells, 50ft x 50ft each. 2 spaces per shell, spliting shell equally.  Placed the shells touching. The calculated infiltration is 0.0400 cfm/ft
- Made two shells, 50ft x 50ft each. 2 spaces per shell, spliting shell equally.  Placed the shells 50 feet apart. The calculated infiltration is 0.0400 cfm/ft
- Made one shell, 100ft x 50ft each. 4 spaces per shell, spliting vertically,such that the zones are the same area/dimensions as the previous examples. The calculated infiltration is 0.0400 cfm/ft in the end cap spaces, and 0.0200 CFM/sf in the middle spaces. This is due to less exterior wall area (as expected).
- Made two shells, 50ft x 50ft each. 2 spaces per shell, same spaces as above.  But – offset the edge of the shells when drawing in wizard mode such that the edge of the spaces were not the edge of the shell(s) (refer to image). Placed the shells such that the two zones were touching. The calculated infiltration is 0.0400 cfm/ft in the end cap spaces, and 0.0200 CFM/sf in the middle spaces; matching as if done in a single shell.

The last example allows the user to change the wall from adiabatic to a heat transfer surface easily. Can also modify the infiltration rate as needed & detailed ablve. PNNL has published several reports on infilatration rates which can be references as well for good information.

Let me (and all of us) know if this seems at odd with previous experiences or overlooked a detail. Thanks in advance.


Thanks,
DARIC R ADAIR PE, CEM, BEMP
Mechanical Engineer, Energy Analyst

Henderson Engineers
Tel (913) 742-5530
daric.adair at hendersonengineers.com<mailto:daric.adair at hendersonengineers.com>

Licensed in KS

From: Bruce Easterbrook [mailto:bruce5 at bellnet.ca]
Sent: Thursday, March 1, 2018 11:19 PM
To: Joe Huang <yjhuang at whiteboxtechnologies.com><mailto:yjhuang at whiteboxtechnologies.com>; equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] Infiltration issues whith more than one shell

Thank's Joe, I didn't realize that.  There are many quirks with DOE2 and eQuest.  I haven't looked at that part of the fine print recently.  Leakage does depend on the wall area and not the floor area in real terms.  Buildings have many different wall heights, plenums or not, ducted or not, etc.  I would guess after normalization that one would have to be careful with how manipulations in geometry are done to achieve other effects in the model.  Infiltration can have a serious effect on a model.
I can remember a past model where I used this technique for an actual butting of 2 industrial spaces/buildings.  The one area was a cable casing thermal setting zone, 1/2 height of the warehouse/machinery high bay zone that was adjacent to it.  I was more concerned with the door and seal between the 2 buildings.  I possibly missed the infiltration difference seeing it was based on floor area and not wall area.   I will have to re-read the fine print.
Bruce
On 3/1/2018 10:32 PM, Joe Huang via Equest-users wrote:

I don't think Bruce's comment is germaine to the problem posed by Menush, since Menush is asking about infiltration and not heat transfer through interior walls.  As far as I know from DOE-2 (always have to add that caveat because I don't work much in eQUEST), infiltration rates are normalized per floor area, rather than external wall area, mainly because that's how the infiltration models have been developed, i.e., effective leakage areas have always been defined as per floor area.  If you don't think that's right, you can always adjust the input values by the ratio of the external wall area to the floor area, as you've described, but then you're on your own in coming up with the correlation,

Joe

Joe Huang

White Box Technologies, Inc.

346 Rheem Blvd., Suite 205A

Moraga CA 94556

yjhuang at whiteboxtechnologies.com<mailto:yjhuang at whiteboxtechnologies.com>

http://weather.whiteboxtechnologies.com for simulation-ready weather data

(o) (925)388-0265

(c) (510)928-2683

"building energy simulations at your fingertips"
On 3/1/2018 6:44 PM, Bruce Easterbrook via Equest-users wrote:
Hi Menush,
I don't think you have the same thing.  eQuest will treat 2 shells butted to each other differently than a single interior wall separating 2 zones in a shell.  It treats the 2 butted walls as exterior walls with a tiny space between.  They are the same wall in your thinking but they are not.  You can delete one of them and make the remaining wall an interior wall and assign the proper butting spaces on each side of the wall as sharing the wall and transferring heating and cooling through the wall.  Or you can add an interior wall to the original space and separate it into 2 zones.  As you have noticed there is a difference in the way eQuest treats your 2 solutions.  It is particular.  Now you need to pick the configuration that matches what you are trying to model in such a way that eQuest does/treats the wall in the way you want it to work.
Bruce Easterbrook P.Eng.
Abode Engineering
On 3/1/2018 5:23 PM, Menush Akbari via Equest-users wrote:
Hi all,

I’m having an issue with infiltration and wondering if anyone else has noticed this. When I’m in wizard mode, I build a very simple rectangular shell and I change the infiltration rate for perimeter zones to 0.05cfm/ft2. I leave the core zone infiltration rate to the eQuest default value (0.001cfm/ft2). From my understanding, the perimeter zone entered value in wizard mode is based on exterior gross wall area. When I move on to detail mode, eQuest changes the value to an infiltration value per floor area instead of exterior wall area. The values so far make sense and I can do the math and get the same numbers eQuest calculates in detail mode. No problems here.

The problem however happens when I create different shells. For example, let’s say I have the same rectangular building as mentioned above, but I split this up into two different shells next to each other (two square shells), therefore one of the walls of each square shell is an interior wall, which means I should not see an infiltration of 0.05 cfm/ft2 of the gross wall area. However when I finish building these two shells in detail mode (which would be identical to one rectangular shell), the infiltration value is not accurate anymore. Instead of the same numbers as my first model (one rectangular shell), the second model calculates an exterior wall infiltration value for the interior walls that are budded up against each other.

Has anyone come across this? Is this a quirk with eQuest and just needs to be changed manually in detail mode, or am I doing something wrong here?

Thanks for the help.

Cheers,

Menush Akbari
BEng, PEng, BEMP, CMVP
Senior Energy Engineer
Mission Green Buildings
(Mission Green Buildings is the trading name of Mission Green Limited)

t. 250 777 3380
makbari at missiongreenbuildings.com<mailto:makbari at missiongreenbuildings.com>
http://missiongreenbuildings.com<http://missiongreenbuildings.com/>

[MGB 5 Years 2]






_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>






_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>






_______________________________________________

Equest-users mailing list

http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org

To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>


________________________________

This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com<mailto:administrator at hendersonengineers.com>.


________________________________

This email and any files transmitted with it are confidential and are intended solely for the use of the individual or entity to whom they are addressed. This communication represents the originator's personal views and opinions, which do not necessarily reflect those of Henderson Engineers, Inc. If you are not the original recipient or the person responsible for delivering the email to the intended recipient, be advised that you have received this email in error, and that any use, dissemination, forwarding, printing, or copying of this email is strictly prohibited. If you received this email in error, please immediately notify administrator at hendersonengineers.com.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180302/b9f47f79/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 6409 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180302/b9f47f79/attachment-0004.jpg>


More information about the Equest-users mailing list