On 7/23/2018 7:21 AM, Bishop, Bill via Equest-users wrote:
>
> Hi Jing,
>
> Your screen shots show that you have entered flowrates for the system supply flow, zonal
> supply flow, zonal outside air and zonal exhaust flow. The error is caused by the zonal
> exhaust flow being greater than the entered system supply flow. You have also selected
> “Track Exhaust Flow” which requires the air handler to supply at least as much air as
> the exhaust requirement. You can do any of the following to eliminate the error:
>
> 1.)Let the system supply flow rate default (leave the input field empty). The system
> will be sized to match the zone exhaust flow (or possibly higher).
>
> 2.)Enter the system supply flow rate to be at least as much as the zone exhaust flow rate.
>
> 3.)Set the zonal exhaust to “No Airflow Tracking” and the EXHAUST-SOURCE to something
> other than “Air Handler”.
>
> Regards,
>
> ~Bill
>
> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP*
>
> *Senior Energy Engineer*
>
> **
>
> Pathfinder-EA-logo-2*/T: (585) 698-1956/**//*F: (585) 325-6005
>
> bbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com>www.pathfinder-ea.com
> <http://www.pathfinder-ea.com/>
>
> 134 South Fitzhugh Street
>
> Rochester, NY 14608 /Ask me why Carbon Fee & Dividend may be right for you./
>
> ******Pathfinder’s Summer Hours begin June 4^th . Our switchboard and office will be
> closed at noon on Fridays through August 31^st .*****
>
> *From:*Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of
> *Brian Fountain via Equest-users
> *Sent:* Monday, July 23, 2018 9:36 AM
> *To:* Jing Hong via Equest-users <hongjing.shirley at gmail.com>
> *Cc:* equest-users at onebuilding.org
> *Subject:* Re: [Equest-users] Evaporative cooler with 100% outside air
>
> Look at the .sim file (view detailed simulation results). There will (likely) be error
> messages at the bottom of that text file relating to why the system/plant module could
> not run,
>
> *From: *Jing Hong via Equest-users
>
> *Sent: *Monday, July 23, 2018 9:31 AM
>
> *To: *equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>;
> equest-users at onebuilding.org <mailto:equest-users at onebuilding.org>
>
> *Reply To: *Jing Hong
>
> *Subject: *[Equest-users] Evaporative cooler with 100% outside air
>
> Dear All,
>
> I have a constant volume 100% outside air evaporative cooler for a kitchen. The CFM is
> 4500. So I set the design flow rate 4500 and outside air flow 4500. When I performed
> simulation, the simulation was terminated due to errors. However, there is no error
> shown in the list of errors. In addition, if I increase the design flow rate above the
> outside air flow rate 4500, then this problem will be gone.
>
> Did anyone have this problem before? How could I fix it?
>
> Thank you!
>
> image.png
>
> image.png
>
> image.png
>
>
> image.png
>
> image.png
>
> Jing Hong
>
> --
>
> School of Architecture and Urban Planning
>
> University of Wisconsin-Milwaukee
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2257 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 2000 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 60829 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 96990 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 83193 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 8828 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0004.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 29923 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0005.png>
More information about the Equest-users
mailing list