[Equest-users] Evaporative cooler with 100% outside air

Joe Huang yjhuang at whiteboxtechnologies.com
Wed Jul 25 19:06:11 PDT 2018


Bill,

I like to compliment you on your very useful diagnosis and explanation of the problem.  
Well done!

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"

On 7/23/2018 7:21 AM, Bishop, Bill via Equest-users wrote:
>
> Hi Jing,
>
> Your screen shots show that you have entered flowrates for the system supply flow, zonal 
> supply flow, zonal outside air and zonal exhaust flow. The error is caused by the zonal 
> exhaust flow being greater than the entered system supply flow. You have also selected 
> “Track Exhaust Flow” which requires the air handler to supply at least as much air as 
> the exhaust requirement. You can do any of the following to eliminate the error:
>
> 1.)Let the system supply flow rate default (leave the input field empty). The system 
> will be sized to match the zone exhaust flow (or possibly higher).
>
> 2.)Enter the system supply flow rate to be at least as much as the zone exhaust flow rate.
>
> 3.)Set the zonal exhaust to “No Airflow Tracking” and the EXHAUST-SOURCE to something 
> other than “Air Handler”.
>
> Regards,
>
> ~Bill
>
> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP*
>
> *Senior Energy Engineer*
>
> **
>
> Pathfinder-EA-logo-2*/T: (585) 698-1956/**//*F: (585) 325-6005
>
> bbishop at pathfinder-ea.com <mailto:wbishop at pathfinder-ea.com>www.pathfinder-ea.com 
> <http://www.pathfinder-ea.com/>
>
> 134 South Fitzhugh Street
>
> Rochester, NY 14608 /Ask me why Carbon Fee & Dividend may be right for you./
>
> ******Pathfinder’s Summer Hours begin June 4^th .  Our switchboard and office will be 
> closed at noon on Fridays through August 31^st .*****
>
> *From:*Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
> *Brian Fountain via Equest-users
> *Sent:* Monday, July 23, 2018 9:36 AM
> *To:* Jing Hong via Equest-users <hongjing.shirley at gmail.com>
> *Cc:* equest-users at onebuilding.org
> *Subject:* Re: [Equest-users] Evaporative cooler with 100% outside air
>
> Look at the .sim file (view detailed simulation results). There will (likely) be error 
> messages at the bottom of that text file relating to why the system/plant module could 
> not run,
>
> *From: *Jing Hong via Equest-users
>
> *Sent: *Monday, July 23, 2018 9:31 AM
>
> *To: *equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>; 
> equest-users at onebuilding.org <mailto:equest-users at onebuilding.org>
>
> *Reply To: *Jing Hong
>
> *Subject: *[Equest-users] Evaporative cooler with 100% outside air
>
> Dear All,
>
> I have a constant volume 100% outside air evaporative cooler for a kitchen. The CFM is 
> 4500. So I set the design flow rate 4500 and outside air flow 4500. When I performed 
> simulation, the simulation was terminated due to errors. However, there is no error 
> shown in the list of errors. In addition, if I increase the design flow rate above the 
> outside air flow rate 4500, then this problem will be gone.
>
> Did anyone have this problem before? How could I fix it?
>
> Thank you!
>
> image.png
>
> image.png
>
> image.png
>
>
> image.png
>
> image.png
>
> Jing Hong
>
> -- 
>
> School of Architecture and Urban Planning
>
> University of Wisconsin-Milwaukee
>
>
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2257 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 2000 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0024.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 60829 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0025.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 96990 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0026.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 83193 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0027.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 8828 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0028.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 29923 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180725/acfa0744/attachment-0029.png>


More information about the Equest-users mailing list