[Equest-users] Evaporative cooler with 100% outside air
Bishop, Bill
bbishop at pathfinder-ea.com
Mon Jul 23 07:21:26 PDT 2018
Hi Jing,
Your screen shots show that you have entered flowrates for the system supply flow, zonal supply flow, zonal outside air and zonal exhaust flow. The error is caused by the zonal exhaust flow being greater than the entered system supply flow. You have also selected “Track Exhaust Flow” which requires the air handler to supply at least as much air as the exhaust requirement. You can do any of the following to eliminate the error:
1.) Let the system supply flow rate default (leave the input field empty). The system will be sized to match the zone exhaust flow (or possibly higher).
2.) Enter the system supply flow rate to be at least as much as the zone exhaust flow rate.
3.) Set the zonal exhaust to “No Airflow Tracking” and the EXHAUST-SOURCE to something other than “Air Handler”.
Regards,
~Bill
William Bishop, PE, BEMP, BEAP, CEM, LEED AP
Senior Energy Engineer
[Pathfinder-EA-logo-2]T: (585) 698-1956 F: (585) 325-6005
bbishop at pathfinder-ea.com<mailto:wbishop at pathfinder-ea.com> www.pathfinder-ea.com<http://www.pathfinder-ea.com/>
[cid:image004.png at 01D4226F.1E4FFDA0]134 South Fitzhugh Street
Rochester, NY 14608 Ask me why Carbon Fee & Dividend may be right for you.
*****Pathfinder’s Summer Hours begin June 4th. Our switchboard and office will be closed at noon on Fridays through August 31st.****
From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of Brian Fountain via Equest-users
Sent: Monday, July 23, 2018 9:36 AM
To: Jing Hong via Equest-users <hongjing.shirley at gmail.com>
Cc: equest-users at onebuilding.org
Subject: Re: [Equest-users] Evaporative cooler with 100% outside air
Look at the .sim file (view detailed simulation results). There will (likely) be error messages at the bottom of that text file relating to why the system/plant module could not run,
From: Jing Hong via Equest-users
Sent: Monday, July 23, 2018 9:31 AM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>; equest-users at onebuilding.org<mailto:equest-users at onebuilding.org>
Reply To: Jing Hong
Subject: [Equest-users] Evaporative cooler with 100% outside air
Dear All,
I have a constant volume 100% outside air evaporative cooler for a kitchen. The CFM is 4500. So I set the design flow rate 4500 and outside air flow 4500. When I performed simulation, the simulation was terminated due to errors. However, there is no error shown in the list of errors. In addition, if I increase the design flow rate above the outside air flow rate 4500, then this problem will be gone.
Did anyone have this problem before? How could I fix it?
Thank you!
[image.png]
[image.png]
[image.png]
[image.png]
[image.png]
Jing Hong
--
School of Architecture and Urban Planning
University of Wisconsin-Milwaukee
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 9336 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0008.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 4600 bytes
Desc: image003.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0028.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image011.png
Type: image/png
Size: 8828 bytes
Desc: image011.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0029.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.jpg
Type: image/jpeg
Size: 2257 bytes
Desc: image002.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0009.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 2000 bytes
Desc: image004.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0030.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image006.png
Type: image/png
Size: 60829 bytes
Desc: image006.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0031.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 96990 bytes
Desc: image008.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0032.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image010.png
Type: image/png
Size: 83193 bytes
Desc: image010.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0033.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image013.png
Type: image/png
Size: 29923 bytes
Desc: image013.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180723/58abd339/attachment-0034.png>
More information about the Equest-users
mailing list