[Equest-users] Modeling DOAS, extremely high heating energy

Lapierre, Patrick plapierre at bpa.ca
Tue Jan 23 12:05:59 PST 2018


Your heating consumption is off chart because eQUEST sized the capacity of your system to an absurd value, resulting in an abysmal part load ratio. I’m not sure why eQUEST overrides the capacity you entered though.

To fix it, you need to specify the flow of your DOAS (either in the system and the zone) and ensure they work at 100% OA.

See modified files for system RTU-1 which runs fine now.


[Bouthillette Parizeau]<http://www.bpa.ca/>

Patrick Lapierre_ing. BEMP
plapierre at bpa.ca | t: 5143833747x2807


De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Michael Campbell via Equest-users
Envoyé : 23 janvier 2018 14:49
À : equest-users <equest-users at lists.onebuilding.org>
Objet : [Equest-users] Modeling DOAS, extremely high heating energy

Hi eQUEST Users,
I am modeling a DOAS system.
I've used the dummy zone approach and I've set thermostat schedules for the dummy zones which are intended to control the supply air temperature of the DOAS systems.

I have checked all my inputs and believe they are correct, however I am getting extremely high energy usage from the DOAS units.
I'm hoping someone can take a few minutes to review my model and let me know what is causing this high heating energy?

My files are attached.

Thank you,
Mike
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180123/3f79b219/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.jpg
Type: image/jpeg
Size: 1706 bytes
Desc: image001.jpg
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180123/3f79b219/attachment-0004.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 16132_New Market West - Proposed.pd2
Type: application/octet-stream
Size: 101250 bytes
Desc: 16132_New Market West - Proposed.pd2
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180123/3f79b219/attachment-0008.obj>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 16132_New Market West - Proposed.inp
Type: application/octet-stream
Size: 321924 bytes
Desc: 16132_New Market West - Proposed.inp
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180123/3f79b219/attachment-0009.obj>


More information about the Equest-users mailing list