[Equest-users] [EnergyPlus_Support] RE: White Box Technologies brings simulation weather data to the satellite age

Joe Huang yjhuang at whiteboxtechnologies.com
Mon Jan 8 15:44:37 PST 2018


The rain and snow flags are still available in the raw weather station data, but haven't 
been included in the processed weather files since the 1990's because  everyone in this 
hemisphere at least have adopted the TMY2/TMY3 formats, in content  if not the literal 
file format, developed by NREL, which does not include these two flags. I was also under 
the impression that none of the simulation programs, such as DOE-2, do not use these two 
flags anyway.   If these flags are of use, it would make sense to include them, which 
would not require a change in the DOE-2 *.BINM format, but would require a change to the 
EnergyPlus *.epw format.

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 205A
Moraga CA 94556
yjhuang at whiteboxtechnologies.com
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"

On 1/8/2018 12:15 PM, 'Jones, Christopher' christopher.r.jones at wsp.com 
[EnergyPlus_Support] wrote:
>
> I have a question – what happened to the rain and snow flags that were in the old CWEC 
> file but are missing in the latest versions. Many snow melting systems have a snow/rain 
> sensor in the slab used to trigger the system on.
>
> **
>
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
> T +1 416-644-0252
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4 Canada
>
> wsp.com
>
> __
>
> **
>
> /Please consider the environment before printing.../
>
> *From:*Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf Of 
> *Joe Huang via Equest-users
> *Sent:* Tuesday, January 02, 2018 10:15 PM
> *To:* Nicholas Caton <Nicholas.Caton at schneider-electric.com>; BLDG-SIM 
> <bldg-sim at lists.onebuilding.org>; EnergyPlus_Support 
> <EnergyPlus_Support at yahoogroups.com>; equest-users at onebuilding.org
> *Cc:* Jim Dirkes <jim at buildingperformanceteam.com>
> *Subject:* Re: [Equest-users] White Box Technologies brings simulation weather data to 
> the satellite age
>
> Nick,
>
> This is an interesting topic that has evolved in an unexpected way.  Now that NREL has 
> mastered the technology of satellite-derived solar radiation, they have regarded weather 
> station data as an impediment, since there's no way to get such measured data to match 
> the 5-kilometer grid of the satellite-derived solar. Therefore, they have abandoned the 
> weather station data (which was was used in all the TMYs to date) and gone instead to 
> Reanalysis Data from NOAA's MERRA, which is running a climate forecasting model in 
> retrospective mode. I don't have time now to discuss reanalysis, except to say that from 
> what I've seen the results are decidedly "iffy".  Almost two years ago, I managed to get 
> a Work Statement through ASHRAE  for someone to take a good look at reanalysis data.
>
> So, what does this mean for your question?   NREL's National Solar Radiation Data Base 
> (NSRDB) can now get you the hourly time series or a TMY for more than a million grid 
> points over the US, all with satellite-derived solar radiation but  MERRA results for 
> the other climate parameters.  I've told NREL several years ago that for the building 
> simulation industry it would be much better to merge the  satellite-derived solar with 
> actual station data that give good accurate coverage of urban areas where buildings are 
> located. NREL's response was that they'd be happy to do this, but someone has to pay 
> them for the work.
>
> In response to your hypothesis below, I think you're being too disparaging of the 
> previous modeling efforts while raising too high your expectations of satellite solar.  
> It's not that the previous models failed to account for local climate conditions, but 
> that they lacked good data to drive them.  For example, all models included terms for 
> cloud cover and clearness, or for the more detailed physical models arcane parameters 
> like aerosol optical depth, preciptable moisture, etc.,  but how available are the input 
> data and how reliable are they?  The advantages of satellite-derived solar are that they 
> provide a comprehensive and objective view of the cloud conditions, which combined with 
> satellite measurements of the atmospheric conditions and  improved modeling, results in  
> accuracies that previous modeling efforts can not attain.  As far as discerning 
> localized effects of smog and dust in urban areas, that would still depend on whether 
> there's sufficient monitoring at that spatial and time scale to detect the differences. 
> What I mean is that it's one thing to observe that in general urban locations have more 
> smog and particulates than rural locations, but it's something else to quantify the 
> resultant differences in solar radiation over time and distance.
>
> I'd like to take the opportunity here to step back and comment on the status of weather 
> data for the building energy community, My interactions with NREL has brought the 
> realization that we have been piggy-backing on the efforts of others outside our 
> community for our weather data.  I don't intend to pick on the NREL Solar Program, 
> several of whom I consider friends and colleagues, but their target client is the solar 
> power industry.  Since solar power arrays can be installed anywhere, preferably in rural 
> uninhabited locations, it makes sense to go to satellite-derived solar.  It's also clear 
> that to serve that industry, NREL would focus its efforts on getting the best solar 
> values, while all the other climatic parameters, like temperature, humidity, wind speed, 
> etc., are secondary, which may be why getting them from MERRA is a satisfactory choice.  
> The focus on solar is also evident in the weighting used by NREL to develop the TMYs, 
> with 50% weight placed on the 2 solar and 50% on the remaining 8 non-solar parameters.
>
> For the building energy community, or priorities are somewhat different. Since 99% of 
> buildings are located in urban locations, we should focus much more on climate in urban 
> areas.  Luckily, that's also where the great majority of existing weather are located, 
> which is why I'm resistant to throwing out measured weather data and replacing them with 
> synthetic data, no matter how much they've been "seeded" with real data. As for the 
> weighting of climate parameters in selecting the typical months,  why not use building 
> energy simulations and weight them by the distribution of heating and cooling loads?
>
> Joe
>
> Joe Huang
> White Box Technologies, Inc.
> 346 Rheem Blvd., Suite 205A
> Moraga CA 94556
> yjhuang at whiteboxtechnologies.com <mailto:yjhuang at whiteboxtechnologies.com>
> http://weather.whiteboxtechnologies.com  for simulation-ready weather data
> (o) (925)388-0265
> (c) (510)928-2683
> "building energy simulations at your fingertips"
>
> On 1/2/2018 9:30 AM, Nicholas Caton wrote:
>
>     Hi Joe,
>
>     From your perspective, are NREL or any other government/professional bodies making
>     moves/indications to update/refresh the current TMY3 sets to utilize
>     satellite-derived solar radiation? Seems like a no-brainer for our industry, but is
>     there a counter-argument?  It seems likely, but has there been rigorous comparisons
>     of satellite-derived solar radiation against measured values and/or our
>     “present-day” solar models used to derive solar radiation information for building
>     energy simulation?
>
>     Also, I’m trying to understand and correctly characterize the impact of this
>     development in simple terms my brain can follow.  Is it fair to say:
>
>     The solar models used in developing weather files for building energy simulations
>     to-date in our industry (including all/most industry-standard TMY weather sets),
>     because they have been using solar radiation derived from (evolving) solar models,
>     have _not_ accounted for the likes of local climate cloud cover / smog / dust? 
>     Seattle (~47°N) has perhaps been seeing as much sunlight through the winter as Paris
>     (~48°N)?
>
>     Does satellite-derived solar radiation address some or all of these local climate
>     issues (cloud cover, smog, dust) affecting direct/indirect solar radiation?
>
>     Thanks sincerely for all your teaching Joe,
>
>     ~Nick
>
>     *Nick Caton, P.E., BEMP*
>
>     Senior Energy Engineer
>     Regional Energy Engineering Manager
>
>     Energy and Sustainability Services
>     Schneider Electric
>
>     	
>
>     D 913.564.6361
>     M 785.410.3317
>     F 913.564.6380
>     E nicholas.caton at schneider-electric.com <mailto:nicholas.caton at schneider-electric.com>
>
>     	
>
>     15200 Santa Fe Trail Drive
>     Suite 204
>     Lenexa, KS 66219
>     United States
>
>     *From:*Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On Behalf
>     Of *Joe Huang via Equest-users
>     *Sent:* Thursday, December 14, 2017 8:13 PM
>     *To:* BLDG-SIM <bldg-sim at lists.onebuilding.org>
>     <mailto:bldg-sim at lists.onebuilding.org>; EnergyPlus_Support
>     <EnergyPlus_Support at yahoogroups.com> <mailto:EnergyPlus_Support at yahoogroups.com>;
>     equest-users at lists.onebuilding.org <mailto:equest-users at lists.onebuilding.org>
>     *Subject:* [Equest-users] White Box Technologies brings simulation weather data to
>     the satellite age
>
>     It is with joy and some trepidation to report that White Box Technologies (WBT) is
>     updating all its historical weather files with satellite-derived solar radiation.
>     Joy because this overcomes what has been the most significant question mark with
>     weather files; trepidation because of the amount of work needed to carry out and
>     maintain this effort. To show that this is more than marketing hype, I need to give
>     a rather long explanation about this development.
>
>     The bane of weather data over the past three decades has been the solar radiation
>     (global horizontal and direct normal) which are not measured parameters, but derived
>     using various solar and sky models. All the familiar "typical year" sets, i.e., TMY,
>     WYEC, IWEC, etc., let alone the historical weather files, have modeled solar
>     radiation. Although a lot of
>     work has gone into such models (see M. Iqbal,"An Introduction to Solar Radiation",
>     Academic Press, 1983), there remain an almost intractible problem of the lack of
>     good measured solar to tune any of these models. For example, in the ASHRAE IWEC2
>     weather files, my team was able to find one or two years' measured data for less
>     than 50 locations,
>     from which were derived 28 sets of regression coefficients then used for all 3,012
>     IWEC2 locations.
>
>     For the past decade and a half, researchers around the world have been working to
>     derive solar radiation from weather satellite imagery, driven largely by the needs
>     of the solar power industry for the siting of solar power plants and getting
>     "bankable" solar estimates for their arrays. Our little building energy simulation
>     sector can of course benefit by hanging on the coattails of the solar power
>     industry, but the downside has been to be totally priced out, since the commercial
>     cost for one year's solar data for one location (grid cell) typically runs around
>     $1,000.
>
>     A welcome development over the last five years is that various government offices or
>     affiliated consortia are now beginning to also providing access to satellite-derived
>     solar radiation at minimal or more acceptable costs under various conditions. Over
>     the past three years, WBT has obtained access to such data and permission for its
>     use in WBT weather files.
>     WBT is now either replacing the solar radiation on its historical weather files, or
>     using satellite-derived radiation to develop custom solar coefficients for each
>     location to extend the satellite-derived solar to time periods outside the available
>     time window. With the exception of polar locations above or below 60/66 degrees,
>     island nations in the Pacific and Indian Ocean, and a few unfortunate "blind spots",
>     the entire land mass is being covered with at least 10 years up to 18 years of
>     hourly solar records.
>
>     Starting in 2018, WBT historical weather files in the following areas will all have
>     satellite-derived solar radiation for the following time periods: Europe, Africa,
>     South America east of 66 West, i.e., Brazil and Uruguay (2004 to date), Australia
>     (1999 to date), and East Asia (2007 to date, access pending). WBT historical weather
>     files in the following areas will have satellite-derived solar radiation for the
>     indicated time periods - North America and Central/South American down to 20 South
>     (1998-2015), South Asia (2000-2014), with modeled solar radiation from 2016 on that
>     has been individually tuned to the past satellite-derived solar.
>
>     Another benefit to the satellite-derived solar is to increases the number of
>     available weather stations, which in many places has been limited by the lack of
>     cloud cover data needed to model the solar radiation. For reasons that are not
>     immediately identifiable, several English-speaking Commonwealth countries has seen a
>     marked drop in the number of available stations due to the decreases in the
>     reporting of cloud cover (see plot, ZAF = South Africa). For example, the number of
>     stations in the UK has dropped by almost 2/3s between 2001 and 2017 (174 to 64), but
>     with satellite-derived solar, it will go back up to over 180, while in Australia and
>     South Africa the comparable numbers are from 175 to well over 500, and from 37 to
>     over 100, respectively.
>
>     If interested, customers who have purchased a historical weather files from WBT over
>     the past five years can get an updated weather file at no cost. Lastly, although it
>     will take at least a month to update all 10,000 2017 files, it's very quick to do
>     for any specific location or even 50 or so locations. Therefore, if you have an
>     urgent request please e-mail me and I will put that at the beginning of the queue
>     for that day.
>
>     -- 
>
>     Joe Huang
>
>     White Box Technologies, Inc.
>
>     346 Rheem Blvd., Suite 205A
>
>     Moraga CA 94556
>
>     yjhuang at whiteboxtechnologies.com <mailto:yjhuang at whiteboxtechnologies.com>
>
>     http://weather.whiteboxtechnologies.com  for simulation-ready weather data
>
>     (o) (925)388-0265
>
>     (c) (510)928-2683
>
>     "building energy simulations at your fingertips"
>
>
> ------------------------------------------------------------------------------------------
>
>
> NOTICE: This communication and any attachments ("this message") may contain information 
> which is privileged, confidential, proprietary or otherwise subject to restricted 
> disclosure under applicable law. This message is for the sole use of the intended 
> recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, 
> dissemination or distribution of, or reliance on, this message is strictly prohibited. 
> If you have received this message in error, or you are not an authorized or intended 
> recipient, please notify the sender immediately by replying to this message, delete this 
> message and all copies from your e-mail system and destroy any printed copies. You are 
> receiving this communication because you are listed as a current WSP contact. Should you 
> have any questions regarding WSP's electronic communications policy, please consult our 
> Anti-Spam Commitment at www.wsp.com/casl <http://www.wsp.com/casl>. For any concern or 
> if you believe you should not be receiving this message, please forward this message to 
> caslcompliance at wsp.com <mailto:caslcompliance at wsp.com> so that we can promptly address 
> your request. Note that not all messages sent by WSP qualify as commercial electronic 
> messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir 
> des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à 
> divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif 
> du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, 
> reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu 
> ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, 
> veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie 
> électronique ou imprimée. Vous recevez cette communication car vous faites partie des 
> contacts de WSP. Si vous avez des questions concernant la politique de communications 
> électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au 
> www.wsp.com/lcap <http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que 
> vous ne devriez pas recevoir ce message, prière de le transférer au 
> conformitelcap at wsp.com <mailto:conformitelcap at wsp.com> afin que nous puissions 
> rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis 
> par WSP qui constituent des messages electroniques commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl
> __._,_.___
> ------------------------------------------------------------------------------------------
> Posted by: "Jones, Christopher" <Christopher.r.Jones at wsp.com>
> ------------------------------------------------------------------------------------------
> Reply via web post 
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/messages/37879;_ylc=X3oDMTJxajJicWVxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzM3ODc5BHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTUxNTQ0MjU2MQ--?act=reply&messageNum=37879> 
> 	• 	Reply to sender 
> <mailto:Christopher.r.Jones at wsp.com?subject=RE%3A%20%5BEquest-users%5D%20White%20Box%20Technologies%20brings%20simulation%20weather%20data%20to%20the%20satellite%20age> 
> 	• 	Reply to group 
> <mailto:EnergyPlus_Support at yahoogroups.com?subject=RE%3A%20%5BEquest-users%5D%20White%20Box%20Technologies%20brings%20simulation%20weather%20data%20to%20the%20satellite%20age> 
> 	• 	Start a New Topic 
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/newtopic;_ylc=X3oDMTJlMWdkbGppBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTUxNTQ0MjU2MQ--> 
> 	• 	Messages in this topic 
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/topics/37869;_ylc=X3oDMTM2bjlnNGs2BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzM3ODc5BHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTUxNTQ0MjU2MQR0cGNJZAMzNzg2OQ--> 
> (4)
>
> ------------------------------------------------------------------------------------------
> Check out the automatic photo album with 2 photo(s) 
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/photos/photomatic/788930472;_ylc=X3oDMTE4M3R1OW82BF9TAzk3MzU5NzE0BGNmOQNQSE9UT01BVElDBHNlYwNtZWdhcGhvbmU-> 
> from this topic.
> image003.png image003.png 
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/photos/photomatic/788930472;_ylc=X3oDMTE4M3R1OW82BF9TAzk3MzU5NzE0BGNmOQNQSE9UT01BVElDBHNlYwNtZWdhcGhvbmU-> 
>
> ------------------------------------------------------------------------------------------
> Have you tried the highest rated email app? <https://yho.com/1wwmgg>
> With 4.5 stars in iTunes, the Yahoo Mail app is the highest rated email app on the 
> market. What are you waiting for? Now you can access all your inboxes (Gmail, Outlook, 
> AOL and more) in one place. Never delete an email again with 1000GB of free cloud storage.
> ------------------------------------------------------------------------------------------
> EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support at gard.com
>
> The EnergyPlus web site is found at:
> http://www.energyplus.net/
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed 
> connection.  Limit attachments to small files.
>
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation 
> link and press the "search" button.
> Visit Your Group 
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlbmFlcm9tBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTUxNTQ0MjU2MQ--> 
>
>
>   * New Members
>     <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmZjN2YmRvBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE1MTU0NDI1NjE->
>     1
>
> Yahoo! Groups 
> <https://groups.yahoo.com/neo;_ylc=X3oDMTJkYzZoN2MxBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNTE1NDQyNTYx> 
>
> • Privacy <https://info.yahoo.com/privacy/us/yahoo/groups/details.html> • Unsubscribe 
> <mailto:EnergyPlus_Support-unsubscribe at yahoogroups.com?subject=Unsubscribe> • Terms of 
> Use <https://info.yahoo.com/legal/us/yahoo/utos/terms/>
>
> .
>
> __,_._,___

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180108/54c4990d/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180108/54c4990d/attachment-0016.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image002.png
Type: image/png
Size: 255 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180108/54c4990d/attachment-0017.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.png
Type: image/png
Size: 8477 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180108/54c4990d/attachment-0018.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image004.png
Type: image/png
Size: 12088 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180108/54c4990d/attachment-0019.png>


More information about the Equest-users mailing list