[Equest-users] System 4 - PSZHP Unmet Hours - "undefined" thermostat schedules
umesh atre
umeshatre at gmail.com
Wed Feb 14 09:13:30 PST 2018
Thanks Bill. Guess I need some more coffee :)
On Wed, Feb 14, 2018 at 9:49 AM, Bishop, Bill <bbishop at pathfinder-ea.com>
wrote:
> When you set the zone COOL/HEAT-TEMP-SCH to “undefined”, there is no
> thermostat control in the zone and no unmet cooling/heating hours will be
> reported because the system is not trying to maintain the zone at any
> particular temperature. The cooling and/or heating thermostat schedules
> should be defined for at least the control zone of a single zone system.
>
> ~Bill
>
>
>
> *William Bishop, PE, BEMP, BEAP, CEM, LEED AP **|** Pathfinder Engineers
> & Architects LLP*
>
> *Senior Energy Engineer*
>
>
>
>
>
> 134 South Fitzhugh Street
> <https://maps.google.com/?q=134+South+Fitzhugh+Street%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%0D+Rochester,+NY+14608&entry=gmail&source=g>
> Rochester, NY 14608
> <https://maps.google.com/?q=134+South+Fitzhugh+Street%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%C2%A0%0D+Rochester,+NY+14608&entry=gmail&source=g>
>
> *T: (585) 698-1956 <(585)%20698-1956>* F: (585)
> 325-6005
>
> bbishop at pathfinder-ea.com <wbishop at pathfinder-ea.com>
> www.pathfinder-ea.com
>
> [image: http://png-5.findicons.com/files/icons/977/rrze/720/globe.png]Carbon
> Fee and Dividend - simple, effective, and market-based.
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] *On
> Behalf Of *umesh atre via Equest-users
> *Sent:* Wednesday, February 14, 2018 10:26 AM
> *To:* Rybl, Vicki <vrybl at rdkengineers.com>
> *Cc:* equest-users at onebuilding.org
> *Subject:* Re: [Equest-users] System 4 - PSZHP Unmet Hours
>
>
>
> Hi Vicki,
>
>
>
> When I run your model, I get unmet hours for all except PSZ 9. After
> looking a bit further, this seems to be the only one with no Heat (or Cool)
> Temp Schedule defined.
>
> If you revert the schedules back to the default 'undefined' for all
> systems, all unmet hours go away. I am not sure what this means, but does
> look schedule related.
>
> Hoping this helps,
>
> Take care,
>
> Umesh
>
>
>
>
>
>
>
>
>
>
>
> On Wed, Feb 14, 2018 at 8:10 AM, Rybl, Vicki via Equest-users <
> equest-users at lists.onebuilding.org> wrote:
>
> Thanks Chris – how did you deal with economizer inputs for the PTHP system?
>
>
>
> John – weather file is attached.
>
>
>
> *Vicki Rybl, LEED AP BD+C, Fitwel Ambassador* | Energy Engineer | *RDK
> Engineers, An NV5 Company* <http://www.nv5.com/>
>
> 70 Fargo Street, Suite 800 | Boston, MA 02210
> <https://maps.google.com/?q=70+Fargo+Street,+Suite+800+%7C+Boston,+MA+02210&entry=gmail&source=g>
> | P: 857.221.5943 <(857)%20221-5943> | F: 617.345.4226 <(617)%20345-4226>
>
>
>
> Electronic Communications Disclaimer
> <http://www.nv5.com/contact-us/electronic-communications-disclaimer/>
>
>
>
> *From:* Jones, Christopher [mailto:Christopher.r.Jones at wsp.com]
> *Sent:* Wednesday, February 14, 2018 8:14 AM
> *To:* John Aulbach <jra_sac at yahoo.com>; Rybl, Vicki <
> vrybl at RDKEngineers.com>
> *Cc:* equest-users at onebuilding.org
> *Subject:* RE: [Equest-users] System 4 - PSZHP Unmet Hours
>
>
>
> I had the same problem with the PSZ HP system using 3.65.7173. I
> eventually gave up and switched to PTAC HP and the under heated hours
> disappeared.
>
>
>
>
>
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
>
>
> T +1 416-644-0252 <(416)%20644-0252>
>
>
>
> 2300 Yonge Street, Suite 2300
> <https://maps.google.com/?q=2300+Yonge+Street,+Suite+2300%0D+Toronto,+ON+M4P+1E4+Canada&entry=gmail&source=g>
>
> Toronto, ON M4P 1E4 Canada
> <https://maps.google.com/?q=2300+Yonge+Street,+Suite+2300%0D+Toronto,+ON+M4P+1E4+Canada&entry=gmail&source=g>
>
> wsp.com
>
>
>
>
>
> *Please consider the environment before printing...*
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *John Aulbach
> via Equest-users
> *Sent:* Tuesday, February 13, 2018 3:38 PM
> *To:* equest-users at lists.onebuilding.org; Rybl, Vicki <
> vrybl at RDKEngineers.com>
> *Subject:* Re: [Equest-users] System 4 - PSZHP Unmet Hours
>
>
>
> Would you please send us your weather file also. I cannot seem to get it
> to download.
>
>
>
> Thanks.
>
>
>
> John
>
>
>
> On Tuesday, February 13, 2018, 12:27:43 PM PST, Rybl, Vicki via
> Equest-users <equest-users at lists.onebuilding.org> wrote:
>
>
>
>
>
> Here are the model files.
>
>
>
> *Vicki Rybl, LEED AP BD+C, Fitwel Ambassador* | Energy Engineer | *RDK
> Engineers, An NV5 Company* <http://www.nv5.com/>
>
> 70 Fargo Street, Suite 800 | Boston, MA 02210
> <https://maps.google.com/?q=70+Fargo+Street,+Suite+800+%7C+Boston,+MA+02210&entry=gmail&source=g>
> | P: 857.221.5943 <(857)%20221-5943> | F: 617.345.4226 <(617)%20345-4226>
>
>
>
> Electronic Communications Disclaimer
> <http://www.nv5.com/contact-us/electronic-communications-disclaimer/>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *John Aulbach
> via Equest-users
> *Sent:* Tuesday, February 13, 2018 1:54 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] System 4 - PSZHP Unmet Hours
>
>
>
> Vicki:
>
>
>
> Would you kindly send the Group your .INP and .PD2 files, so we can help
> you?
>
>
>
> John R. Aulbach, PE
>
>
>
> On Tuesday, February 13, 2018, 10:34:27 AM PST, Rybl, Vicki via
> Equest-users <equest-users at lists.onebuilding.org> wrote:
>
>
>
>
>
> eQuesters:
>
>
>
> We’re working on a 90.1-2007 baseline model with System 4: PSZ-HP. It’s
> modeled as a Packaged Single Zone system with DX cooling and Heat Pump
> heat. Unmet hours in all zones are through the roof, around 6,000. We’ve
> gone through all our usual methods to mitigate unmet hours to no avail
> (zone entering temp, schedules, total airflow, zone heat source, feels like
> we’ve changed every input available?).
>
>
>
> If the heat source is switched to electric or furnace, the unmet hours
> disappear. In addition, the design is a VRF system that’s being modeled as
> a PSZ heat pump and has no unmet hours.
>
>
>
> Has anyone run into this issue? What are we missing?
>
>
>
> Any insight is appreciated.
>
>
>
>
>
>
>
> *Vicki Rybl, LEED AP BD+C, Fitwel Ambassador* | Energy Engineer | *RDK
> Engineers, An NV5 Company* <http://www.nv5.com/>
>
> 70 Fargo Street, Suite 800 | Boston, MA 02210
> <https://maps.google.com/?q=70+Fargo+Street,+Suite+800+%7C+Boston,+MA+02210&entry=gmail&source=g>
> | P: 857.221.5943 <(857)%20221-5943> | F: 617.345.4226 <(617)%20345-4226>
>
>
>
> Electronic Communications Disclaimer
> <http://www.nv5.com/contact-us/electronic-communications-disclaimer/>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> ------------------------------
>
>
>
> NOTICE: This communication and any attachments ("this message") may
> contain information which is privileged, confidential, proprietary or
> otherwise subject to restricted disclosure under applicable law. This
> message is for the sole use of the intended recipient(s). Any unauthorized
> use, disclosure, viewing, copying, alteration, dissemination or
> distribution of, or reliance on, this message is strictly prohibited. If
> you have received this message in error, or you are not an authorized or
> intended recipient, please notify the sender immediately by replying to
> this message, delete this message and all copies from your e-mail system
> and destroy any printed copies. You are receiving this communication
> because you are listed as a current WSP contact. Should you have any
> questions regarding WSP's electronic communications policy, please consult
> our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you
> believe you should not be receiving this message, please forward this
> message to caslcompliance at wsp.com so that we can promptly address your
> request. Note that not all messages sent by WSP qualify as commercial
> electronic messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »),
> peut contenir des renseignements ou de l'information privilégiés,
> confidentiels, propriétaires ou à divulgation restreinte en vertu de la
> loi. Ce message est destiné à l'usage exclusif du/des destinataire(s)
> voulu(s). Toute utilisation non permise, divulgation, lecture,
> reproduction, modification, diffusion ou distribution est interdite. Si
> vous avez reçu ce message par erreur, ou que vous n'êtes pas un
> destinataire autorisé ou voulu, veuillez en aviser l'expéditeur
> immédiatement et détruire le message et toute copie électronique ou
> imprimée. Vous recevez cette communication car vous faites partie des
> contacts de WSP. Si vous avez des questions concernant la politique de
> communications électroniques de WSP, veuillez consulter notre Engagement
> anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez
> que vous ne devriez pas recevoir ce message, prière de le transférer au
> conformitelcap at wsp.com afin que nous puissions rapidement traiter votre
> demande. Notez que ce ne sont pas tous les messages transmis par WSP qui
> constituent des messages electroniques commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl
>
>
>
>
>
> ---------- Forwarded message ----------
> From: Postmaster <>
> To: "equest-users at onebuilding.org" <equest-users at onebuilding.org>
> Cc:
> Bcc:
> Date: Wed, 14 Feb 2018 09:10:54 -0500
> Subject: MA_Lawrence_Muni.bin
>
> *Attachment Notice*
>
> The following attachment was removed from the associated email message.
>
>
>
> File Name
>
> *MA_Lawrence_Muni.bin*
>
> File Size
>
> *148992 Bytes*
>
>
>
> Attachment management policies limit the types of attachments that are
> allowed to pass through the email infrastructure.
>
> Attachments are monitored and audited for security reasons.
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/575be849/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image003.jpg
Type: image/jpeg
Size: 1517 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/575be849/attachment.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image008.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/575be849/attachment.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image007.png
Type: image/png
Size: 3856 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/575be849/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image005.jpg
Type: image/jpeg
Size: 1647 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/575be849/attachment-0001.jpg>
More information about the Equest-users
mailing list