[Equest-users] System 4 - PSZHP Unmet Hours
umesh atre
umeshatre at gmail.com
Wed Feb 14 07:26:25 PST 2018
Hi Vicki,
When I run your model, I get unmet hours for all except PSZ 9. After
looking a bit further, this seems to be the only one with no Heat (or Cool)
Temp Schedule defined.
If you revert the schedules back to the default 'undefined' for all
systems, all unmet hours go away. I am not sure what this means, but does
look schedule related.
Hoping this helps,
Take care,
Umesh
On Wed, Feb 14, 2018 at 8:10 AM, Rybl, Vicki via Equest-users <
equest-users at lists.onebuilding.org> wrote:
> Thanks Chris – how did you deal with economizer inputs for the PTHP system?
>
>
>
> John – weather file is attached.
>
>
>
> *Vicki Rybl, LEED AP BD+C, Fitwel Ambassador* | Energy Engineer | *RDK
> Engineers, An NV5 Company* <http://www.nv5.com/>
>
> 70 Fargo Street, Suite 800 | Boston, MA 02210 | P: 857.221.5943
> <(857)%20221-5943> | F: 617.345.4226 <(617)%20345-4226>
>
>
>
> Electronic Communications Disclaimer
> <http://www.nv5.com/contact-us/electronic-communications-disclaimer/>
>
>
>
> *From:* Jones, Christopher [mailto:Christopher.r.Jones at wsp.com]
> *Sent:* Wednesday, February 14, 2018 8:14 AM
> *To:* John Aulbach <jra_sac at yahoo.com>; Rybl, Vicki
> <vrybl at RDKEngineers.com>
> *Cc:* equest-users at onebuilding.org
> *Subject:* RE: [Equest-users] System 4 - PSZHP Unmet Hours
>
>
>
> I had the same problem with the PSZ HP system using 3.65.7173. I
> eventually gave up and switched to PTAC HP and the under heated hours
> disappeared.
>
>
>
>
>
> *Christopher R. Jones*, P.Eng.
>
> Technical Specialist
>
> Sustainability & Energy
>
>
>
> T +1 416-644-0252 <(416)%20644-0252>
>
>
>
> 2300 Yonge Street, Suite 2300
>
> Toronto, ON M4P 1E4 Canada
>
> wsp.com
>
>
>
>
>
> *Please consider the environment before printing...*
>
>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *John Aulbach
> via Equest-users
> *Sent:* Tuesday, February 13, 2018 3:38 PM
> *To:* equest-users at lists.onebuilding.org; Rybl, Vicki <
> vrybl at RDKEngineers.com>
> *Subject:* Re: [Equest-users] System 4 - PSZHP Unmet Hours
>
>
>
> Would you please send us your weather file also. I cannot seem to get it
> to download.
>
>
>
> Thanks.
>
>
>
> John
>
>
>
> On Tuesday, February 13, 2018, 12:27:43 PM PST, Rybl, Vicki via
> Equest-users <equest-users at lists.onebuilding.org> wrote:
>
>
>
>
>
> Here are the model files.
>
>
>
> *Vicki Rybl, LEED AP BD+C, Fitwel Ambassador* | Energy Engineer | *RDK
> Engineers, An NV5 Company* <http://www.nv5.com/>
>
> 70 Fargo Street, Suite 800 | Boston, MA 02210 | P: 857.221.5943
> <(857)%20221-5943> | F: 617.345.4226 <(617)%20345-4226>
>
>
>
> Electronic Communications Disclaimer
> <http://www.nv5.com/contact-us/electronic-communications-disclaimer/>
>
>
>
> *From:* Equest-users [mailto:equest-users-bounces at lists.onebuilding.org
> <equest-users-bounces at lists.onebuilding.org>] *On Behalf Of *John Aulbach
> via Equest-users
> *Sent:* Tuesday, February 13, 2018 1:54 PM
> *To:* equest-users at lists.onebuilding.org
> *Subject:* Re: [Equest-users] System 4 - PSZHP Unmet Hours
>
>
>
> Vicki:
>
>
>
> Would you kindly send the Group your .INP and .PD2 files, so we can help
> you?
>
>
>
> John R. Aulbach, PE
>
>
>
> On Tuesday, February 13, 2018, 10:34:27 AM PST, Rybl, Vicki via
> Equest-users <equest-users at lists.onebuilding.org> wrote:
>
>
>
>
>
> eQuesters:
>
>
>
> We’re working on a 90.1-2007 baseline model with System 4: PSZ-HP. It’s
> modeled as a Packaged Single Zone system with DX cooling and Heat Pump
> heat. Unmet hours in all zones are through the roof, around 6,000. We’ve
> gone through all our usual methods to mitigate unmet hours to no avail
> (zone entering temp, schedules, total airflow, zone heat source, feels like
> we’ve changed every input available?).
>
>
>
> If the heat source is switched to electric or furnace, the unmet hours
> disappear. In addition, the design is a VRF system that’s being modeled as
> a PSZ heat pump and has no unmet hours.
>
>
>
> Has anyone run into this issue? What are we missing?
>
>
>
> Any insight is appreciated.
>
>
>
>
>
>
>
> *Vicki Rybl, LEED AP BD+C, Fitwel Ambassador* | Energy Engineer | *RDK
> Engineers, An NV5 Company* <http://www.nv5.com/>
>
> 70 Fargo Street, Suite 800 | Boston, MA 02210 | P: 857.221.5943
> <(857)%20221-5943> | F: 617.345.4226 <(617)%20345-4226>
>
>
>
> Electronic Communications Disclaimer
> <http://www.nv5.com/contact-us/electronic-communications-disclaimer/>
>
>
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
> ------------------------------
>
>
>
> NOTICE: This communication and any attachments ("this message") may
> contain information which is privileged, confidential, proprietary or
> otherwise subject to restricted disclosure under applicable law. This
> message is for the sole use of the intended recipient(s). Any unauthorized
> use, disclosure, viewing, copying, alteration, dissemination or
> distribution of, or reliance on, this message is strictly prohibited. If
> you have received this message in error, or you are not an authorized or
> intended recipient, please notify the sender immediately by replying to
> this message, delete this message and all copies from your e-mail system
> and destroy any printed copies. You are receiving this communication
> because you are listed as a current WSP contact. Should you have any
> questions regarding WSP's electronic communications policy, please consult
> our Anti-Spam Commitment at www.wsp.com/casl. For any concern or if you
> believe you should not be receiving this message, please forward this
> message to caslcompliance at wsp.com so that we can promptly address your
> request. Note that not all messages sent by WSP qualify as commercial
> electronic messages.
>
> AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »),
> peut contenir des renseignements ou de l'information privilégiés,
> confidentiels, propriétaires ou à divulgation restreinte en vertu de la
> loi. Ce message est destiné à l'usage exclusif du/des destinataire(s)
> voulu(s). Toute utilisation non permise, divulgation, lecture,
> reproduction, modification, diffusion ou distribution est interdite. Si
> vous avez reçu ce message par erreur, ou que vous n'êtes pas un
> destinataire autorisé ou voulu, veuillez en aviser l'expéditeur
> immédiatement et détruire le message et toute copie électronique ou
> imprimée. Vous recevez cette communication car vous faites partie des
> contacts de WSP. Si vous avez des questions concernant la politique de
> communications électroniques de WSP, veuillez consulter notre Engagement
> anti-pourriel au www.wsp.com/lcap. Pour toute question ou si vous croyez
> que vous ne devriez pas recevoir ce message, prière de le transférer au
> conformitelcap at wsp.com afin que nous puissions rapidement traiter votre
> demande. Notez que ce ne sont pas tous les messages transmis par WSP qui
> constituent des messages electroniques commerciaux.
>
>
>
> -LAEmHhHzdJzBlTWfa4Hgs7pbKl
>
>
>
>
> ---------- Forwarded message ----------
> From: Postmaster <>
> To: "equest-users at onebuilding.org" <equest-users at onebuilding.org>
> Cc:
> Bcc:
> Date: Wed, 14 Feb 2018 09:10:54 -0500
> Subject: MA_Lawrence_Muni.bin
> *Attachment Notice*
>
> The following attachment was removed from the associated email message.
>
> File Name
> *MA_Lawrence_Muni.bin*
> File Size
> *148992 Bytes*
>
> Attachment management policies limit the types of attachments that are
> allowed to pass through the email infrastructure.
>
> Attachments are monitored and audited for security reasons.
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/62fb883b/attachment.html>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: not available
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/62fb883b/attachment.png>
More information about the Equest-users
mailing list