[Equest-users] System 4 - PSZHP Unmet Hours

Rybl, Vicki vrybl at RDKEngineers.com
Wed Feb 14 06:10:50 PST 2018


Thanks Chris – how did you deal with economizer inputs for the PTHP system?

John – weather file is attached.

Vicki Rybl, LEED AP BD+C, Fitwel Ambassador | Energy Engineer | RDK Engineers, An NV5 Company<http://www.nv5.com/>
70 Fargo Street, Suite 800 | Boston, MA 02210 | P: 857.221.5943 | F: 617.345.4226

Electronic Communications Disclaimer<http://www.nv5.com/contact-us/electronic-communications-disclaimer/>

From: Jones, Christopher [mailto:Christopher.r.Jones at wsp.com]
Sent: Wednesday, February 14, 2018 8:14 AM
To: John Aulbach <jra_sac at yahoo.com>; Rybl, Vicki <vrybl at RDKEngineers.com>
Cc: equest-users at onebuilding.org
Subject: RE: [Equest-users] System 4 - PSZHP Unmet Hours

I had the same problem with the PSZ HP system using 3.65.7173. I eventually gave up and switched to PTAC HP and the under heated hours disappeared.


Christopher R. Jones, P.Eng.
Technical Specialist
Sustainability & Energy

[cid:image001.png at 01D3A573.B4D18B50]
T +1 416-644-0252

2300 Yonge Street, Suite 2300
Toronto, ON M4P 1E4 Canada
wsp.com


Please consider the environment before printing...


From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach via Equest-users
Sent: Tuesday, February 13, 2018 3:38 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>; Rybl, Vicki <vrybl at RDKEngineers.com<mailto:vrybl at RDKEngineers.com>>
Subject: Re: [Equest-users] System 4 - PSZHP Unmet Hours

Would you please send us your weather file also. I cannot seem to get it to download.

Thanks.

John

On Tuesday, February 13, 2018, 12:27:43 PM PST, Rybl, Vicki via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:



Here are the model files.



Vicki Rybl, LEED AP BD+C, Fitwel Ambassador | Energy Engineer | RDK Engineers, An NV5 Company<http://www.nv5.com/>

70 Fargo Street, Suite 800 | Boston, MA 02210 | P: 857.221.5943 | F: 617.345.4226



Electronic Communications Disclaimer<http://www.nv5.com/contact-us/electronic-communications-disclaimer/>



From: Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] On Behalf Of John Aulbach via Equest-users
Sent: Tuesday, February 13, 2018 1:54 PM
To: equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>
Subject: Re: [Equest-users] System 4 - PSZHP Unmet Hours



Vicki:



Would you kindly send the Group your .INP and .PD2 files, so we can help you?



John R. Aulbach, PE



On Tuesday, February 13, 2018, 10:34:27 AM PST, Rybl, Vicki via Equest-users <equest-users at lists.onebuilding.org<mailto:equest-users at lists.onebuilding.org>> wrote:





eQuesters:



We’re working on a 90.1-2007 baseline model with System 4: PSZ-HP. It’s modeled as a Packaged Single Zone system with DX cooling and Heat Pump heat. Unmet hours in all zones are through the roof, around 6,000. We’ve gone through all our usual methods to mitigate unmet hours to no avail (zone entering temp, schedules, total airflow, zone heat source, feels like we’ve changed every input available?).



If the heat source is switched to electric or furnace, the unmet hours disappear. In addition, the design is a VRF system that’s being modeled as a PSZ heat pump and has no unmet hours.



Has anyone run into this issue? What are we missing?



Any insight is appreciated.







Vicki Rybl, LEED AP BD+C, Fitwel Ambassador | Energy Engineer | RDK Engineers, An NV5 Company<http://www.nv5.com/>

70 Fargo Street, Suite 800 | Boston, MA 02210 | P: 857.221.5943 | F: 617.345.4226



Electronic Communications Disclaimer<http://www.nv5.com/contact-us/electronic-communications-disclaimer/>





_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

_______________________________________________
Equest-users mailing list
http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
To unsubscribe from this mailing list send  a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG<mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>

________________________________


NOTICE: This communication and any attachments ("this message") may contain information which is privileged, confidential, proprietary or otherwise subject to restricted disclosure under applicable law. This message is for the sole use of the intended recipient(s). Any unauthorized use, disclosure, viewing, copying, alteration, dissemination or distribution of, or reliance on, this message is strictly prohibited. If you have received this message in error, or you are not an authorized or intended recipient, please notify the sender immediately by replying to this message, delete this message and all copies from your e-mail system and destroy any printed copies. You are receiving this communication because you are listed as a current WSP contact. Should you have any questions regarding WSP's electronic communications policy, please consult our Anti-Spam Commitment at www.wsp.com/casl<http://www.wsp.com/casl>. For any concern or if you believe you should not be receiving this message, please forward this message to caslcompliance at wsp.com<mailto:caslcompliance at wsp.com> so that we can promptly address your request. Note that not all messages sent by WSP qualify as commercial electronic messages.

AVIS : Ce message, incluant tout fichier l'accompagnant (« le message »), peut contenir des renseignements ou de l'information privilégiés, confidentiels, propriétaires ou à divulgation restreinte en vertu de la loi. Ce message est destiné à l'usage exclusif du/des destinataire(s) voulu(s). Toute utilisation non permise, divulgation, lecture, reproduction, modification, diffusion ou distribution est interdite. Si vous avez reçu ce message par erreur, ou que vous n'êtes pas un destinataire autorisé ou voulu, veuillez en aviser l'expéditeur immédiatement et détruire le message et toute copie électronique ou imprimée. Vous recevez cette communication car vous faites partie des contacts de WSP. Si vous avez des questions concernant la politique de communications électroniques de WSP, veuillez consulter notre Engagement anti-pourriel au www.wsp.com/lcap<http://www.wsp.com/lcap>. Pour toute question ou si vous croyez que vous ne devriez pas recevoir ce message, prière de le transférer au conformitelcap at wsp.com<mailto:conformitelcap at wsp.com> afin que nous puissions rapidement traiter votre demande. Notez que ce ne sont pas tous les messages transmis par WSP qui constituent des messages electroniques commerciaux.



-LAEmHhHzdJzBlTWfa4Hgs7pbKl

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/477d6b2e/attachment-0002.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image001.png
Type: image/png
Size: 25844 bytes
Desc: image001.png
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/477d6b2e/attachment-0004.png>
-------------- next part --------------
An embedded message was scrubbed...
From: Postmaster <>
Subject: MA_Lawrence_Muni.bin
Date: Wed, 14 Feb 2018 09:10:54 -0500
Size: 1355
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20180214/477d6b2e/attachment-0002.eml>


More information about the Equest-users mailing list