I came across this problem before.
As you pointed out, changing the MaxExpDeps didn't work for me.
In the end I deleted every interior wall to reduce the number of components in the model and it worked.
Not ideal but it was better than not running at all.
Patrick Lapierre_ing. BEMP
plapierre at bpa.ca | t: 5143833747x2807
-----Message d'origine-----
De : Equest-users [mailto:equest-users-bounces at lists.onebuilding.org] De la part de Brian Fountain via Equest-users
Envoyé : 4 février 2018 09:31
À : equest-users at lists.onebuilding.org
Objet : [Equest-users] Maximum number of expression dependency lists exceeded
I know this has come up on the list before but I am now struggling with a (large, over-zoned) model that is throwing "Maximum number of expression dependency lists exceeded" errors.
The archive suggested setting MaxExpDeps=10 in the .pd2. That does not change the number of errors thrown on my model.
Would greatly appreciate assistance from anyone who has overcome this.
Many thanks,
Brian