[Equest-users] mystery heating load
Joe Huang
yjhuang at whiteboxtechnologies.com
Thu Dec 20 12:59:55 PST 2018
And the cause for the mystery load is ?? Don't just leave us hanging!
Joe
On 12/20/2018 12:47 PM, Chris Hadlock via Equest-users wrote:
> Thanks to all who responded...the problem has now been solved. My
> faith in eQuest remains.
>
> Chris
>
> On Thu, Dec 20, 2018 at 2:33 PM David Eldridge via Equest-users
> <equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>> wrote:
>
> That last sentence is the issue – the system is providing some
> amount of air including return and OA to the space, without a
> heating coil, meanwhile the thermostat may be expecting 70F all of
> the time.
>
> The issue could be resolved by “upgrading” the unit to heat,
> removing/reducing the OA quantity, or by relaxing or removing the
> thermostat schedules depending on what your goals are for the project.
>
> David
>
> *David S. Eldridge, Jr.**, P**.**E**.**, LEED AP BD+C, BEMP, BEAP,
> HBDP*
>
> Associate
>
> Direct: (847) 316-9224| Mobile: (773) 490-5038
>
> *Grumman/Butkus Associates*| 820 Davis Street, Suite 300 |
> Evanston, IL 60201
>
> Energy Efficiency Consultants and Sustainable Design Engineers
>
> _grummanbutkus.com <http://grummanbutkus.com/>_| _Blog
> <http://grummanbutkus.com/blog>_ | _Facebook
> <https://www.facebook.com/pages/GrummanButkus-Associates/1385285015032526>_
> | _Twitter <https://twitter.com/grummanbutkus>_
>
> *From:*Equest-users
> [mailto:equest-users-bounces at lists.onebuilding.org
> <mailto:equest-users-bounces at lists.onebuilding.org>] *On Behalf Of
> *Chris Hadlock via Equest-users
> *Sent:* Thursday, December 20, 2018 1:05 PM
> *To:* equest-users at lists.onebuilding.org
> <mailto:equest-users at lists.onebuilding.org>
> *Subject:* Re: [Equest-users] mystery heating load
>
> I've had a few responses requesting the modeling files so I've
> attached the INP and PD2 file (weather file is CWEC\Toronto.bin).
> The zone in question is "L0 Elev Lobby S" and I've already removed
> all exterior surfaces from this space (i.e. there are no Child
> Components). I've assigned this zone to it's own system (it's the
> last system on the air-side tab) called "Test System". I've
> already created the hourly reports where you'll see all of the
> underheated hours (which only occur in the winter). The LS-B
> report shows no (zero) htg load. I realize the system is not
> really providing any heating to this zone the way it's setup.
>
> Thanks,
>
> Chris
>
> On Thu, Dec 20, 2018 at 1:26 PM Chris Hadlock <cjhadlock at gmail.com
> <mailto:cjhadlock at gmail.com>> wrote:
>
> Hello,
>
> I've created a model using eQuest 3.65 (DOE 2.2) build 7173
> that is of a 20 storey multi-residential building located in
> Toronto, Ontario (Canada). There is a basement with a elevator
> lobby that is an interior space (no exterior walls).
>
> My model keeps telling me I have underheated hours for this
> lobby. I'm trying to figure out why there is a heating load
> and I'm stumped. I have removed what I believe to be all
> potential sources of heat loss. I've deleted the underground
> floor (which was R-100 anyway), I've deleted the interior
> walls (just to be thorough), there is no infiltration, and
> I've set the ventilation to zero. In my mind, there is no
> source of heat loss. I've even added a significant (10 W/ft2)
> equipment load and yet there are still underheated hours (I've
> even reduced my Tstat setpoint to 60F).
>
> I've run an hourly report to help figure out the loads for
> both the space ("Sum of all weighted loads except infil and
> latent") and zone ("Load Calc'd SPACE Sensible load at const
> temp (Btu/hr)"). These reports all indicate a positive load
> (i.e. net heat gain) from my lights, plug loads and occupants.
> However through this process I'm also questioning these
> reports as the lighting, people and equipment load being
> reported don't exactly align with my modeled schedules for
> these loads....but I've put a pin in that.
>
> Regardless, I have no idea how to figure out what may be
> resulting in net heat loss for this zone. To be thorough, I
> checked the elevator lobby on the ground level and the same
> thing is happening. Has anybody seen this before...any ideas
> what might be causing heat loss for a zone with no ventilation
> and no walls and no infiltration? It does seem to be seasonal
> (i.e no underheated hours in the summer) so it has some
> connection to weather file but does not correlate exactly.
>
> If you do take the time to read this, a big thank you. If you
> provide the answer, you'll for sure be on Santa's "nice" list.
>
> Chris
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to
> EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
> <mailto:EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG>
>
>
> _______________________________________________
> Equest-users mailing list
> http://lists.onebuilding.org/listinfo.cgi/equest-users-onebuilding.org
> To unsubscribe from this mailing list send a blank message to EQUEST-USERS-UNSUBSCRIBE at ONEBUILDING.ORG
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.onebuilding.org/pipermail/equest-users-onebuilding.org/attachments/20181220/4b5cf077/attachment.html>
More information about the Equest-users
mailing list